RE: Ambulatory Health Care protection

2020-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Is it light hazard? If so, yes. Is it existing? May not have to upgrade. From: Sprinklerforum On Behalf Of Thomas Reinhardt via Sprinklerforum Sent: Friday, June 26, 2020 1:17 PM To: sprinklerforum@lists.firesprinkler.org Cc: Thomas Reinhardt Subject: FW: Ambulatory Health Care protection

RE: Tablet or 4K monitor for viewing PDFs?

2020-06-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I currently have set up (2) 43” 4K TV and one 27” monitor. They work well. You still pan and zoom, but you have a lot more on the screen at a time. Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298

RE: Uprights in non combustible concealed space

2020-06-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I could be wrong, but isn’t there something in IFC that states a fire protection system left in place needs to be compliant for the area? I’ve had inspectors interpret as you indicate. It’s the rationale that you can’t leave dead sprinkler pipe in the air. Now, I have had this same

RE: Protecting A 500 Degree 12' x 10' Oven

2020-06-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Dry system – all threaded. I doubt the coupling or flange rubbers would handle the heat. We’ve done similar situations. Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION:

RE: [EXTERNAL] RE: Floor area less than required

2020-06-16 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
] RE: Floor area less than required The spec is demanding 8.0K for the LH areas. Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via

RE: [EXTERNAL] RE: Floor area less than required

2020-06-16 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
4.2k or even 2.8k can be your friend – if applicable. Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 NEW MOBILE: 480-272-2471

RE: Fertilizer Storage

2020-06-08 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Or maybe one of the other many standards in the NFPA family?? Been awhile since I looked into fertilizer storage. From: Sprinklerforum On Behalf Of Brian Harris via Sprinklerforum Sent: Monday, June 8, 2020 8:06 AM To: sprinklerforum@lists.firesprinkler.org Cc: Brian Harris Subject:

RE: [External] Re: I-B construction - ABS plumbing piping

2020-05-21 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
klerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Wednesday, May 20, 2020 6:36 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Cc: Travis Mack, SET, CFPS, CWBSP,

RE: I-B construction - ABS plumbing piping

2020-05-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
-G via Sprinklerforum Sent: Tuesday, May 19, 2020 2:55 PM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack, SET, CFPS, CWBSP, RME-G ; 'Matt Grise' ; 'Rocci 3 Cetani' Subject: RE: I-B construction - ABS plumbing piping Yeah. That is the conundrum we are in. From: Sprinklerforum

RE: I-B construction - ABS plumbing piping

2020-05-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
rum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Tuesday, May 19, 2020 4:39 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G

I-B construction - ABS plumbing piping

2020-05-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
We have a fairly good sized school project. Plumber ran ABS drain piping. Electrician has some cabling not in conduit. Inspector is stating the space is now combustible and requires sprinklers above all ceiling areas. Has anyone run into this and how was it resolved? Drawings and specs

RE: Spacing ESFR-17 Sprinkler at new interior wall

2020-03-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
was already there. FM signed off on it so who am I to argue. By the way I tried moving back up the line, but with 2'-6" between sprinkler and bar joist on each side, I was 5 sprinklers back and it still wasn't working out. -----Original Message- From: Travis Mack,

RE: Spacing ESFR-17 Sprinkler at new interior wall

2020-03-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I’m not saying it won’t work. But, there is nothing you have to hang your hat on should there ever be an issue. I always tell customers to figure moving 3-5 sprinklers on a branch line whenever you have a wall cause ESFR issues. Travis Mack, CFPS, CWBSP,

RE: Boat and RV storage units

2020-03-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
eCbHNRijI%3D=0> https://www.linkedin.com/in/travismack "The bitterness of poor quality remains long after the sweetness of low price is forgotten." From: Steve Leyton Sent: Wednesday, March 18, 2020 12:11 PM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack, SET, CFPS, CWBS

Boat and RV storage units

2020-03-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
What densities is everyone doing these type of projects? If doing as low piled storage, are you taking the QR reduction for these type of facilities? Just curious what everyone is doing these days for these units. Travis Mack, CFPS, CWBSP, RME-G, SET MFP

RE: Minimum Lead-in Sizing

2020-03-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
gotten." From: Spencer Tomlinson Sent: Wednesday, March 18, 2020 10:53 AM To: Steve Leyton ; sprinklerforum@lists.firesprinkler.org Cc: Travis Mack, SET, CFPS, CWBSP, RME-G Subject: RE: Minimum Lead-in Sizing Yes sir - of the exact same opinion, as well as Matt's "what does it

RE: Minimum Lead-in Sizing

2020-03-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
: Steve Leyton Sent: Wednesday, March 18, 2020 10:36 AM To: sprinklerforum@lists.firesprinkler.org Cc: Matthew J Willis ; Travis Mack, SET, CFPS, CWBSP, RME-G ; 'Spencer Tomlinson' Subject: RE: Minimum Lead-in Sizing Huh? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprink

RE: Minimum Lead-in Sizing

2020-03-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
What is the reference for a minimum 4"? We've had several smaller than that over my career. Never had an issue that I know of. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700

RE: Dedicated space in Electrical Rooms per NEC Article 110

2020-03-04 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Steve: I don’t believe the NEC indicates dry piping as a method of protection in your case. So, you will need the drip pans or something similar. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION:

RE: Quick FM question

2020-03-03 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Not that I have ever seen. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 fax: 866-430-6107 tm...@mfpdesign.com www.mfpdesign.com Send large

Corrugated Metal Deck - smooth??

2020-02-17 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I have a customer that intended to use horizontal sidewall sprinklers under an exposed corrugated metal deck. The deck is < 3" in depth. The EOR on the project has rejected it, stating sidewalls must be under a smooth ceiling and the corrugated metal deck does not meet the criteria for a smooth

RE: TYCO RM-1

2020-02-09 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
That is what I have always used. Just friction loss through length plus the 3 psi. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 fax: 866-430-6107

RE: BIM Woes

2020-01-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
nkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Matthew J Willis Sent: Wednesday, January 15, 2020 12:54 PM To: sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton ; 'Travis Mack, SET, CFPS, CWBSP, RME-G' ;

RE: Pipe adjacent to duct

2020-01-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Bob: I believe that is in Section 9.3 which is the seismic section. This job is Seismic Design Category B, so 9.3 doesn’t apply. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext.

RE: [EXTERNAL] Pipe adjacent to duct

2020-01-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Exactly. It’s all up in the air. It was a BIM job and not an issue with anyone during coordination. Now it’s all up in the air installed and seems to be an issue. You can’t win some days. Plus, it shouldn’t be an issue at all, but now it is. Travis Mack,

RE: inside hose - Standpipes

2020-01-07 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
prinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Tuesday, January 7, 2020 2:12 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Cc: Travis Mack, SET, CFPS

inside hose - Standpipes

2020-01-07 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I have an AHJ that is requesting inside hose allowance to be provided at the standpipe hose valves. I recall there being standards in 13 or 14 that states you are not required to provided inside hose allowances because of standpipes. Can someone help me locate. It would not normally be an

RE: Panel Construction

2019-12-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
If you have typical metal deck, then you have to fill the "flutes" with mineral wool or something similar. Panel construction requires heat doesn't pass over the top of the members. Typical metal deck will allow that to happen if the spaces aren't filled with a noncombustible material.

RE: 2016 NFPA 13 Reference help

2019-12-06 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
m: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Friday, December 06, 2019 11:31 AM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Cc: Travis Mack, SET, CFPS,

2016 NFPA 13 Reference help

2019-12-06 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Regarding sidewall sprinklers, I recall a section stating that sidewall sprinklers can not be in the throw pattern of another sidewall sprinkler. Can some one help me locate that section? I'm drawing a blank today on search. Travis Mack, CFPS, CWBSP, RME-G, SET

RE: [EXTERNAL] RE: Trouble getting Architects to give Revit files

2019-12-04 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
ZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=VKA9bmHyPeFp2FY2au6X-yd_m3iPAkSdkziKuk5Vz_g=K1QlWaq1qqGSRHw1TkBMRf9MEqKbatUGPJ6ypbJlZOg= udHelp/cloudhelp/2019/ENU/Revit-Model/files/GUID-C61C2E42-0561-48C9-8459-3EA C10EC8E16-htm.html Not as nice as native Revit file

RE: Trouble getting Architects to give Revit files

2019-12-02 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Haven't had much push back. The thing I hate is when they strip out the sheet sets. But, we typically get the model. It is in all of our quotes that it is to be provided when the project is drawn in REVIT. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ

RE: Interstitial Spaces

2019-10-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Is it a concealed space? If so, is it combustible or non-combustible? NFPA 13 will consider a building fully sprinklered while allowing sprinklers not be installed in all areas. Does your space meet the criteria to be exempted from sprinklers? Travis Mack,

RE: Upright Sprinkler

2019-10-08 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
That is for CMSA only. Using standard spray, you want to look at 8.6.5.2.1.8. That is the reference for smaller than 3” not needing to meet the 3x rule. For 3” and larger, you must comply with 3x rule for standard spray. Travis Mack, CFPS, CWBSP, RME-G, SET

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
ips, Mark Sent: Friday, September 20, 2019 5:00 PM To: sprinklerforum@lists.firesprinkler.org; vi...@wtfp.net Cc: Matthew J Willis ; Travis Mack, SET, CFPS, CWBSP, RME-G Subject: Re: COMBUSTIBLE CEILING SPACE Is there any code reference because I lost the argument several times. Le

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
It is my understanding you can use the ceiling with the pendent sprinklers as the floor level when measuring the QR reduction. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Criteria for QR reduction: QR sprinklers Light / Ord hazard Wet System Height ≤20’ No unprotected ceiling pockets If you concealed combustible space meets those criteria, then you can do the QR reduction. Note: If you have a concealed space that requires specially listed sprinklers,

RE: Pump? Or Pump & Tank?

2019-09-12 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Brian: You say the insurance guy is saying Grp A on racks. 25’ storage 30’ ceiling. Chapter 15 is solid piled / palletized. 0.45/2500 is 12’ storage up to 15’ ceiling. I think you are a bit off there based on your description. Chap 17 is rack storage of plastics. Location has meaning.

RE: N1.85 graph paper

2019-08-27 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
he forms are on the NFPA site. Just spent the last hour looking for them, the location is not obvious. -Original Message----- From: Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org> > To: sprinklerforum mailto:sprinklerforum@lists.f

RE: N1.85 graph paper

2019-08-27 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
If you go to the NFPA website, you can buy the e-forms for NFPA 13. It is like $8. They are fillable PDF forms. You get Owner’s Information Certificate Seismic bracing calculation form Hydraulic report sheets Storage sprinkler design checklist Plan review check list Above ground and

RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
to:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Wednesday, August 14, 2019 6:32 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Cc: Travis Mack, SET, CFPS, CWBSP,

RE: Captive Aire Systems

2019-08-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
r, with a small backflow device. You can’t run a restaurant without water, so there is no concern about water system not being monitored. Best. On Aug 14, 2019, at 15:19, Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org> > wrote: I

RE: [EXTERNAL] Captive Aire Systems

2019-08-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
e sweetness of low price is forgotten.” From: Kyle.Montgomery Sent: Wednesday, August 14, 2019 3:27 PM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack, SET, CFPS, CWBSP, RME-G Subject: RE: [EXTERNAL] Captive Aire Systems I’ve always been under the impression that these are

Captive Aire Systems

2019-08-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I’m sure some of you have dealt with these Captive Aire / Piranha systems. Basically they are hood systems that connect to the sprinkler system. The one I have a data sheet for has an operating pressure of 32-70 psi and flows vary depending on # of nozzles. How do those of you dealing with these

RE: Backflow Prevention Valves

2019-08-13 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
If you have hydrants downstream of your BFP device, that is your method of providing full flow forward testing, right? Similar to how a pump test header serves as your means of accomplishing forward flow test. So, if no hydrants downstream of BFP device, then do you need to provide a test

RE: Can a Branchline cross the main when Bracing

2019-08-08 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Airplane = Center fed tree system Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com www.mfpdesign.com Send large files to us via:

RE: CBC / CFC vs NFPA 13

2019-07-24 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Codes supersede standards Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com www.mfpdesign.com Send large files to us via:

partial systems - running piping through unprotected areas

2019-07-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
My memory is failing me today. Isn't there a section that says I can't run piping through un-protected areas? We have a building that has a partially protected basement. Basically, we have to bulk across the basement to protect 3 areas. Can some one help me find the section of 13 that says

RE: EC Heads in an FM Job

2019-07-11 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
There are a ton of specifics with FM and Ex Cov. If you are not familiar, you should likely spend a few hours reviewing 2-0, 3-0 and 3-26 before you go down a rabbit hole and lose a ton of time. Minimum spacings, minimum pressures, minimum in design areas, etc. There are a lot of things

RE: Hazard

2019-07-03 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Owner information certificate is your friend. Have them fill out specifically what is used for. You may fall into EH criteria. Don't you love the kind of stuff we all seem to fall into? Happy July 4th to all. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design,

RE: Sleeping rooms in a hospital

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
't see how you can use residential sprinklers. Perhaps a thoughtfully crafted RFI to the specifying engineer would draw out what I'm SURE will be a most entertaining narrative. SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SE

RE: Where to fine lowest mean temp info

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Use the tables in Chap 10. That is what the NFSA people told me back in the day when figuring temps to use for anti-freeze and DW calcs. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Sleeping rooms in a hospital

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
e typos and voice text corruptions.) Original message ---- From: "Travis Mack, SET, CFPS, CWBSP, RME-G" mailto:tm...@mfpdesign.com> > Date: 6/28/19 12:45 PM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject:

Sleeping rooms in a hospital

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Residential sprinklers or QR? I-2 occupancy. Specs call for residential. I've always done these as QR. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Attic sprinklers

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
to what is in the space. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) On Jun 28, 2019 at 1:40 PM, mailto:st...@protectiondesign.com> > wrote: Or a Viking rep … From: Sprinklerforum [mailto:sprink

RE: Attic sprinklers

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
e: Or a Viking rep … From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Friday, June 28, 2019 10:39 AM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: At

RE: Attic sprinklers

2019-06-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Yes. If occupied, I would say it is not an attic any longer. If there is no ceiling, it is not a concealed space. These are specially listed concealed space sprinklers. A call to Tyco technical services would clear it up for you if that is not enough.

RE: [EXTERNAL] Welded outlets - Equivalent feet

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
MAO, SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Wednesday, June 26, 2019 11:30 AM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: [EXTERNAL]

RE: [EXTERNAL] Welded outlets - Equivalent feet

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
ttp://www.jacobs.com/> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Wednesday, June 26, 2019 12:58 PM To: sprinkler

Welded outlets - Equivalent feet

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Does anyone have a data sheet with the equivalent feet to use in hydraulic calculations. I have a PE reviewing plans (already approved by local AHJ), that is not allowing the fittings used in our program. Our program just uses the tee in NFPA 13. Never mind we have at least 20 psi margins in

RE: FM 8-9

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
l design coverage 94 sq. ft.? -Original Message----- From: Travis Mack, SET, CFPS, CWBSP, RME-G mailto:tm...@mfpdesign.com> > To: sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org> > Sent: Wed, Jun 26, 2019 11:57 am Subject: RE: FM 8-9 I’d have to find the ref

RE: FM 8-9

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
iginal Message----- From: Travis Mack, SET, CFPS, CWBSP, RME-G < <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com> To: sprinklerforum < <mailto:sprinklerforum@lists.firesprinkler.org> sprinklerforum@lists.firesprinkler.org> Sent: Wed, Jun 26, 2019 11:57 am Subject: RE

RE: FM 8-9

2019-06-26 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I’d have to find the reference for you, but it is in FM 3-00. Basically, you do the following: 1 – Design area is # of sprinklers x max area of coverage per sprinkler. So if you have 100 sq ft max, then 10 sprinklers is 1000 sq ft. 2 – Design area is 1.2 x DA^0.5 – unless you have one of

RE: PDF to DWG programs

2019-06-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I am no revit expert by any means, but I believe you can import a PDF into revit and use as a background. As long as it is a vector PDF, but I could be very wrong on that. I am not a Revit guru. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E

RE: obstruction

2019-06-19 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
What type of sprinkler are you using? ESFR - check the ESFR sections. I don't do a lot of CMSA, so I have to look them up every time, but maybe something in CMSA. If you are talking SSU/SSP then I think it would be a stretch to require that. Travis Mack, CFPS,

RE: [EXTERNAL] Re: Suction Control Valve

2019-06-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
o:sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Tuesday, June 18, 2019 4:39 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Suction Control Valve Every case I’ve had one

RE: Suction Control Valve

2019-06-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Every case I've had one is because the water purveyor required it. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com www.mfpdesign.com

RE: PDF to DWG programs

2019-06-18 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Older versions of AutoCAD do it as well. I believe it came in somewhere around 2015 or in that vicinity. If you can’t afford that, there is something like “anydwg” or something along those lines that I used to use before AutoCAD created the PDFIMPORT function.

RE: Questions about FDC's

2019-05-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
The FDC is to supplement, not replace in a fire sprinkler system. There is no requirement to upsize per NFPA 13. NFPA 14 has different requirements. Check that standard for inlet number. You may need bigger size to accommodate flows. Travis Mack, CFPS, CWBSP,

RE: [EXTERNAL] RE: Pump & Tank Fed From a Well

2019-05-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
prinkler.org] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Wednesday, May 22, 2019 12:12 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: [EXTERNAL] RE: Pump & Tank Fed From a Well My first thought goes to dr

RE: Pump & Tank Fed From a Well

2019-05-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
My first thought goes to dry system in the attic. Assuming pitch >2:12 you are calculating 2535 sq ft. This will end up being about 25-30 sprinklers with all of the attic spacing criteria. Dry system = K5.6 sprinklers, so 25 sprinklers * 15 gpm each *1.3 for over discharge gets you to a demand

RE: ESFR and Obstructions - Sizing

2019-05-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
nklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Wednesday, May 22, 2019 9:05 AM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: ESFR and Obstructions - Sizing Can some one help me l

RE: ESFR and Obstructions - Sizing

2019-05-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
his information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents. From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS

ESFR and Obstructions - Sizing

2019-05-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Can some one help me locate the section in NFPA 13 (2016 preferred) that indicates when you have obstructions below the ESFR sprinklers, you supply the sprinkler below the obstruction with pipe size the same as the branch line and you don't include the additional sprinklers in the calculations?

RE: Water Test From Storage Tank

2019-05-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Computer models do it all the time. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com www.mfpdesign.com Send large files to us via:

RE: NFPA 13 8.15.23 Spaces above ceilings 2016ed

2019-04-29 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I'm not sure I get your total picture, but I'll try. First, we start with sprinklers in all spaces. Then we can ask if we can omit in places. The section you quote is only applicable if it is open on one side, like figure A.15.23.3. If your IT room is the space in question and you have it

RE: Intent of 23.4.4.2.5

2019-04-23 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I’ve run into a few AHJs that have specifically thrown this section to us for paint booths. We also had this thrown at us on a tire carousel storage. This caused total havoc on the projects. The paint booth was in an existing facility designed to OH2. They paint booth had 6 sprinklers.

RE: Intent of 23.4.4.2.5

2019-04-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Monday, April 22, 2019 3:23 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Intent of 23.4.4.2.5

RE: Intent of 23.4.4.2.5

2019-04-22 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
This section has been in since 2013 and it has caused some issues. If you are doing room design and meet the requirements for room design then you are done. If you are doing density / area and you only have 1000 sq ft, where the required design area would be 1950 sq ft, then as I

RE: Branchline Restraint

2019-04-11 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Yes. That state agency can be a real pain. I’ve had that happen that my customer stated, just change it to a listed anchor and we will put it in to just make them go away. That’s why I was thinking to have it listed. Travis Mack, CFPS, CWBSP, RME-G, SET MFP

RE: 13R and compartment

2019-04-09 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
some greater application. Ron Greenman rongreen...@gmail.com <mailto:rongreen...@gmail.com> 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Tue, Apr 9,

13R and compartment

2019-04-09 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
If I have a hallway with a 9' ceiling and it opens into an area that goes up to a 12' ceiling, would those be separate compartments? The area with the 12' ceiling is protected by a single sprinkler at 20' spacing, and the hallway has 3 sprinklers at 16' spacing. There is not a true lintel

RE: Dry Pendents Required in Coolers?

2019-04-02 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I won’t say that I haven’t seen people do it before. But, I tend to think you are playing a game that could be a hard pill to swallow if you lose on it. I always indicate dry pendents in those coolers. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC

RE: ESFR and Baffles

2019-04-01 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Yes. There are things you can do to change the building to make it ESFR compatible. But as it was described, you have a building that is not compliant with ESFR. Too many people jump to ESFR as the panacea of storage. Travis Mack, CFPS, CWBSP, RME-G, SET

RE: ESFR and Baffles

2019-04-01 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
design.com From: Sprinklerforum On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Monday, April 1, 2019 11:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: ESFR and Baffles Posting to help a friend. I've always been taught that ESFR is 8' minimum. You are not permitted to

ESFR and Baffles

2019-04-01 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Posting to help a friend. I've always been taught that ESFR is 8' minimum. You are not permitted to use baffles or anything to reduce the minimum distance between ESFR sprinklers. There is a respected FPE challenging this statement and trying to use baffles to allow ESFR to be less than 8'.

RE: Cartoned Group A Plastics

2019-03-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
rk E. Eckard SET Fire Protection Services, LLC 2126 US Hwy. 41 North Perry, GA 31069 Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta) Mobile: 478-244-6653 SYL-216 From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack

RE: Cartoned Group A Plastics

2019-03-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
When needing definitions, Chap 3 of the 2016 is where you want to start. 3.9.1.1 gives your definition of Cartoned. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: [EXTERNAL] RE: Antifreeze temperature requirements

2019-03-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Yes. It is just a mean temperature to use. Are we to use the 100 yr lowest recorded temp? 50 yr? Just lowest in recorded history? Maybe Ice Age temps?  Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271

RE: [EXTERNAL] RE: Antifreeze temperature requirements

2019-03-14 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Chap 10 in NFPA 13 2016 has the isothermal lines. Long ago, I was directed by one of the national organizations to use this map for determining temperatures for freeze protection. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct

RE: Hydrant Flow vs Drain test

2019-03-11 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Just doing the google search that Skyler suggested, it is the first link to pop up. https://axaxl.com/-/media/gaps/e122___0.pdf Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: OS "flow rates"

2019-03-05 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
LMAO!!! You can't make this stuff up. Give him the equivalent foot in 13. Figure out the loss for your flow then give it showing equal. 4 ft' of valve A = 4' of valve B. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ

RE: OS "flow rates"

2019-03-05 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
I've given up trying to figure people out. Some just can't be bothered. There is an equivalent foot chart in NFPA 13 for gate valves. You could give him that for reference. If he is still adamant to see a graph, you could make quick spreadsheet to calculate pressure losses based on

RE: When to Measuring Along the Slope

2019-03-01 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
this case it is 2/12. Bobby Gillett Seago Fire Protection, LLC 850-217-3899 cell 850-836-2288 office 850-836-2277 fax _ From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > on behalf of Travis Mack, SET, CFPS, CWBSP, RME-G mailto

RE: When to Measuring Along the Slope

2019-03-01 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
My conservative opinion is no. You calc on the flat, but space on the slope. So, if your dimension along that slope is 15'-1", then you have exceeded the limits without shifting the sprinkler for small room rule. Travis Mack, CFPS, CWBSP, RME-G, SET MFP

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
For example, not mixing density/area and residential sprinkler calculations. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com Send

RE: Boat Storage

2019-02-21 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Send it to an FPE for a performance based design. There will not be prescriptive standards to address that situation. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Boat Storage

2019-02-21 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Nothing in NFPA standards for it. Check with the insurance company for the project. They may have guidance. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ]

2019-02-06 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
Exhibits are handbook references. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com Send large files to us via:

RE: Piping Passing Over a Panel / Controller

2019-02-06 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Wednesday, February 6, 2019 1:36 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Piping Passing Over a Pa