RE: Odd FP arrangement

2010-02-15 Thread George Church
Can you swap the riser 1 check and control valve so you're tying in without a control valve in the way (unless it’s a DPV above the control valve?) If not, it isn't a huge leap to not see the control valve as a problem when you have two in an acceptable manner -with control valves in the FD path

RE: CPVC and Nail plates

2010-02-15 Thread George Church
I believe in 13R (and other spkr codes) you'll find language requiring protection from mechanical injury one could say makes a nail plate requirement- we didn't' find one in the IRC. Our AHJ was demanding nail plates that were thinker and a lot bigger per the IPC and IMC, even tho they aren't

RE: System Replacement

2010-02-13 Thread George Church
IF they don't store the empties inside, look at the whole of the stored commodity and what's the % Group A? glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Timothy W Goins Sent: Saturday, February 13,

RE: AF Expansion Tanks

2010-02-12 Thread George Church
We don't use perforated pipe hanger stuff cause the code doesn't allow it for our work. Except in 13D, same holds true of expansion tanks, whether they are made of 250 PSI WWP or not, the real question is - are they listed as required by 13 or 13R? The only wiggle room is what might become

RE: Flexible Pipe

2010-02-12 Thread George Church
Can't use hard pipe to make the bends Has he tried using those elbow thingies we often put on the end of a pipe if we want to make a bend? They're far faster and more predictable than bending the pipe. Otherwise, if they're trying to make an odd angle and can't use a pair of 90's to make a

RE: Impaired preaction

2010-02-12 Thread George Church
Yup=- And just plug it with a mech tee when repairs to the detection system are completed. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Vining Sent: Friday, February 12, 2010 11:27 AM To:

RE: System Replacement

2010-02-12 Thread George Church
From the NFSA website: Breaking News! A report direct from the Home Fire Sprinkler Coalition booth at the National Association of Home Builders Show, a segment featuring home fire sprinklers will be aired on ABC this evening at 5:30 EST. Be sure to tune in. glc

RE: pipe sizing question

2010-02-11 Thread George Church
Unless you're doing 13d, how often are you flowing 10 GPM to a head when a 1/2 K5.6 head flows 15 GPM at the min EHP of 7? I can sum it up by quoting what Ken reminds me- It's not what you know, it's what you can prove. As others said, we know what it'll probably be- But without a calc per #13

RE: Beam obstruction rules

2010-02-11 Thread George Church
But his deflector distance was only 6 down from deck, wasn't it? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Michael J. Ricks Sent: Wednesday, February 10, 2010 9:53 PM To:

RE: pipe sizing question

2010-02-11 Thread George Church
. haven't changed since original installation, and that original documentation is available to verify these assumptions. The survey then becomes a change order. On Thu, Feb 11, 2010 at 4:10 AM, George Church for...@ptd.net wrote: Unless you're doing 13d, how often are you flowing 10 GPM to a head when

RE: Beam obstruction rules

2010-02-09 Thread George Church
Spot on- and why we have prescriptive codes to apply- you did- he nneds to understand you comply and that's it, absent clear and present danger, contractual obligations... glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: mixing standard and QR spklrs in calc?

2010-02-09 Thread George Church
, 2010 10:51 AM To: sprinklerforum@firesprinkler.org Subject: RE: mixing standard and QR spklrs in calc? Keep in mind you won't be able to take the QR design reduction based upon ceiling height unless all the sprinklers in your area are QR. Ralphy --- On Mon, 2/8/10, George Church for...@ptd.net

RE: Gas systems replacing sprinklers

2010-02-09 Thread George Church
Or gas with spkr (PA?) backup using higher temp heads, or use concealed to protect against mechanical injury if that's a concern in that environ. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of

RE: Strange piping arrangement

2010-02-08 Thread George Church
Jeez I feel like I should be 20 yrs older for campfire stories. Back before there were 8 dry-pipe valves, we'd routinely tee to a pair and then bring em back together, usually with 8 but if this was a BIG system, then 10 wouldn't cause us to bat an eye. As for design criteria, would have been

L'il Abner-Mattress Tester

2010-02-08 Thread George Church
, flat, as if prepared for a princess and a pea. Owner would prefer not to take .2/1500 to .6 for obvious reasons, one being tenant fitout of a portion of an existing retail center. George Church Rowe Sprinkler ___ Sprinklerforum mailing list

RE: FM Global Data Sheet 2-5

2010-02-05 Thread George Church
So we give this as an outline spec for architects and then bid 13d? Tough to imagine a home large enough to be insured by FM Global Hehe- wall post by the front door with chain and padlock, do they require a diesel? -Original Message- From: sprinklerforum-boun...@firesprinkler.org

help the NAHB!

2010-02-04 Thread George Church
for your assistance in TELLING THEM HOW YOU FEEL!!! George Church Rowe Sprinkler FROM THE PBA: Take 5 minutes and help our cause! PBA has filed a lawsuit in Commonwealth Court to stop implementation of the 2009 building codes, which will add $15,000 to the cost of a new home. We have gotten extensive

sand strainer?

2010-02-04 Thread George Church
in a pump suction application. While I haven't encountered this before, it likely isn't the first time the problem has been encountered. Any one know a remedy other than a tank (with settling basin?) and higher pressure 2,500 GPM pump to make up for the loss of city residual pressure? George Church

RE: sand strainer?

2010-02-04 Thread George Church
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Thursday, February 04, 2010 4:32 PM To: sprinklerforum@firesprinkler.org Subject: sand strainer? We've got a problem child project where

RE: sand strainer?

2010-02-04 Thread George Church
what you're looking for. They claim they can filter out sand. Hellan is the Cadillac so the strainer could be pricey. Regards, James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive Greenville, SC 29607 864.281.5149 George Church for...@ptd.net Sent by: sprinklerforum-boun

RE: sand strainer?

2010-02-04 Thread George Church
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org]on Behalf Of George Church Sent: Thursday, February 04, 2010 5:07 PM To: sprinklerforum@firesprinkler.org Subject: RE: sand strainer? ASCOA paid $22k just expediting an order of em once, they must be Bentleys:) I'll check them

RE: fdc clearance

2010-02-04 Thread George Church
Like the Supreme Court position on pornography- I know it when I see it. If the FDC looks safe to use, its ok. If the picture of YOUR FDC location resembles the one in FPC, then you can't put it there. In an application like this, absent a clear code direction that may appear in a later post and

RE: Interior water storage tank inspections

2010-02-02 Thread George Church
Specialty contractor Iank Industry Consultants, Pgh Tank and Tower, Mumford-Bjorkman Assoc.- There are a lot of them, ranging from contractor to consultant. Robot vrs diver if the tank is still full, etc. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Interior water storage tank inspections

2010-02-02 Thread George Church
That really doesn't give the fitters much expertise in microns, does it? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Craig Leadbetter Sent: Tuesday, February 02, 2010 8:49 AM To:

RE: CPVC in a concealed space

2010-02-02 Thread George Church
Sounds reasonable and prudent, Travis. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Tuesday, February 02, 2010 10:09 AM To: sprinklerforum@firesprinkler.org Subject: CPVC in a

RE: Mansions in the Sky (No Place for NFPA Standards)

2010-02-02 Thread George Church
What makes you think that Oakmont won't be erecting the William Brooks Library of Fire Protection Engineering to house the collection? I'll talk to Ed Rendell. Glc Ps- stay on stationary bicycles and you'll likely hang around here a little longer :) -Original Message- From:

RE: Mansions in the Sky (No Place for NFPA Standards)

2010-02-02 Thread George Church
but another aspect. Listening there Mr. Muncy. More work for you guys. On Tue, Feb 2, 2010 at 9:08 AM, George Church for...@ptd.net wrote: What makes you think that Oakmont won't be erecting the William Brooks Library of Fire Protection Engineering to house the collection? I'll talk to Ed Rendell

RE: Mansions in the Sky (No Place for NFPA Standards)

2010-02-02 Thread George Church
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Tuesday, February 02, 2010 11:51 AM To: sprinklerforum@firesprinkler.org Subject: RE: Mansions in the Sky (No Place for NFPA Standards) I've got a sister in Michigan with a masters

RE: More fires?

2010-02-01 Thread George Church
We had some in the area that border on the ridiculous. 83 yr old man gets a call from his daughter who told him to get out of his apt, the bldg is on fire, she heard it on the scanner. How's that for automatic alarm- can you imagine submitting a procedure to an AHJ that includes a tenant's

RE: Retrofit Questions

2010-01-29 Thread George Church
Do high-rise requirements apply to your building? As an existing bldg, can they be waived? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, January 29, 2010 6:37 AM To:

RE: Elevator machine rooms

2010-01-28 Thread George Church
I recall a GC supt years back noting his SOP was to have an easy to plug location for the elevator shaft sprinklers so they could be readily installed for the FM, removed for the elevator inspector, and left in the manner prescribed by the latter of the two being onsite. glc -Original

Quandry-design to two editions of 13?

2010-01-28 Thread George Church
. What are the rest of you doing to comply? George Church Rowe Sprinkler ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send

RE: Quandry-design to two editions of 13?

2010-01-28 Thread George Church
of NFPA 13? George Church ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send

RE: News Bite

2010-01-25 Thread George Church
This is a job for a trained and experienced professional- And the right one is resident in your state, and she was involved in the passage. Terri Simmons Leyton at PROTECTION DESIGN CONSULTING Ph: 858-751-2930 - ext. 101 -Original Message- From:

RE: Penn Builders Assn Lawsuit

2010-01-22 Thread George Church
...@firesprinkler.org] On Behalf Of Terri Leyton Sent: Friday, January 22, 2010 12:19 PM To: sprinklerforum@firesprinkler.org Subject: RE: Penn Builders Assn Lawsuit George Church - where are you? George was in the den of the PA Builders last night. He was a very special guest speaker at their meeting

RE: Antifreeze Backflow Prevention

2010-01-21 Thread George Church
Didn't matter on Jim's - pump and tank. Assume air gap, since tank non-potable. So drilled check is fine- except when water replaces what dribbled out. As for dry vrs AF, can't use CPVC with dry; dry pend are $$$ and may not fit in small space allotted; in 13d the unlisted bladder is $75, so

RE: Occupancy

2010-01-21 Thread George Church
Sure that wasn't a B52's concert? :) (gee, who was at two last year?) -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton I'm picturing a scene from 20+ years ago with a bunch of those giant

RE: NFPA 20 Suggested Piping Arrangements

2010-01-20 Thread George Church
We include a bypass around the fire pump when supply is from a tank/pump IF THE PUMP FEEDS HYDRANTS ON THE LOOP since the FD can use the gravity source and boost it and make something of it. So it's not just for the sprinklers 8' AFF in the shipping office being fed by the 40' tall tank that we

RE: mixed systems

2010-01-14 Thread George Church
On the other hand, there's a zillion SF of big boxes out there with multiple systems covering ONE area and with 40k SF system limit for high-piled storage, of course more than one system can cover an area. It would only be where different criteria apply and walls pop up that you start worrying

RE: Definition

2010-01-14 Thread George Church
Or the Milwaukee butterball dating back to the 80's -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Thursday, January 14, 2010 4:13 PM To: sprinklerforum@firesprinkler.org Subject: RE:

RE: Definition

2010-01-14 Thread George Church
Move East where its warmer and yes it IS time to go home now and Ken will provide SKITA at no charge to the employee. We could use a nice PE to kick around ;) I checked my iPhone to see if it WAS warmer here tan there today (figured you're about same as Fargo) and indeed, we're 39*F now.

RE: Cure times

2010-01-13 Thread George Church
Impairments are also covered in #25, but it's something you can reference, excerpt and forward to the OWNER to implement- we have enough risk in this business. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of

RE: Arizona State Fire Marshal

2010-01-13 Thread George Church
Well, I understand the state of Michigan decided it couldn't afford the safety of a new code adoption, must be they can't afford a fire marshal in AZ. Course if you look at the deficit, we can't afford the safety of the FDA, FTC, USDA, etc either- we could shut them all down and soon we'll

RE: Arizona State Fire Marshal

2010-01-13 Thread George Church
] Sent: Wednesday, January 13, 2010 2:00 PM To: sprinklerforum@firesprinkler.org Cc: George Church Subject: RE: Arizona State Fire Marshal George, The State of Michigan Office of Fire Safety is still using the 1996 code. Change is a hard sell. George Church for...@ptd.net wrote: Well, I

RE: CA adoption

2010-01-13 Thread George Church
Congrats to T for her efforts, frostbite to you cause you're skiing and I'm working.swooosh-have fun! -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of steve Sent: Wednesday, January 13, 2010 2:17 PM To:

MI

2010-01-13 Thread George Church
to the 1996 NFPA 13 Mike On Wed, Jan 13, 2010 at 2:24 PM, George Church for...@ptd.net wrote: Hang in there, in PA we went from early 80's BOCA until April 2004 adoption of our PA Uniform Construction Code based on 2003 I-codes; 6 years later we led the nation to the IRC. So we went from 20 year

RE: MIC

2010-01-12 Thread George Church
Huguenot, Potter Electric, others will test your samples. You'll need fresh samples, tho and fed ex it to them. The microbes need to have a fighting chance of being alive when the lab gets it. -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Cure times

2010-01-12 Thread George Church
We've held to the 24 hrs since we had Relmark insuring us years ago. If they don't want to, they can sign a release of damage and we'll turn it on 5 minutes after we glue it together (ok, an hour). I think you need about 3 weeks to cure 1 joints in our current weather. There are many of us

RE: Dry Drops

2010-01-12 Thread George Church
Congrats- you just wrote the report for em, sparing him the return paperwork and postage. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Tuesday, January 12, 2010 4:30 PM To:

RE: trailer parked inside

2010-01-07 Thread George Church
If the trailer is in the same exact spot, could a flexible drop be fitted coming down from the roof system and have a bracket rigged to effect an EC HSW pointing into the back of the trailer spraying into it? Then you only have the shielded area below the trailer to either deal with- whether its

RE: trailer parked inside

2010-01-07 Thread George Church
So, does this mean we can't install shell systems in spec buildings because we don't trust them to store other than what the shell is intended for? As I understand it, you're proposing EH2 over the entire, when a localized protection scheme might address the localized hazard of one trailer? How

RE: trailer parked inside

2010-01-07 Thread George Church
Scot- Given the trailer is parked inside a building with what I'll assume is .3/2000 wet system and maybe 20' deck height, would you believe that such a large fire could be produced with control mode sprinklers overhead? Todd- And are the trailers being modified fiberglass bodied or

RE: Fire Pumps FDC's

2010-01-07 Thread George Church
can point to for the GC's sake? Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Wednesday, January 06, 2010 4:20 PM To: sprinklerforum@firesprinkler.org Subject

RE: trailer parked inside

2010-01-07 Thread George Church
I agree the tunnel testing is an interesting discussion. And relevant to a degree to this topic. However, let's again look at the problem- It's ONE trailer parked in a sprinklered building with protection suitable for 14' hi Group A. How many deaths to we expect? The shielded area is likely 8'

RE: Fire Pumps FDC's

2010-01-06 Thread George Church
FDC goes on pump discharge side. Pump not smart enough to know FD took 50 PSI suction from city and boosted it to 150, so now your pump discharge is 250 PSI. Plug pit, install FDC on side of building. -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Dust Ducts

2010-01-06 Thread George Church
http://www.grecon-us.com/pdfs/CC7000_en_usa_web.pdf http://www.argusfirecontrol.com/Products.html http://www.exploguard.com/explo_spark_main.php you can soak what's left after the fire races past your sprinklers if you install standard heads off a wet system; or better, install something like

RE: Electrical Rooms

2010-01-04 Thread George Church
Remember they're the ones finding the invisible fault with you crossing an electrical room with your piping. So that you are sure you comply FULLY with the applicable code preventing you from doing this (ITHO) ask them to provide the applicable code reference. glc -Original Message-

RE: Group 'I' Occupancies

2010-01-04 Thread George Church
That difficult or impossible to evacuate phrase cost a lot of lives in NY State when a group home was protected (over the contractor's objections) to 13D when numerous residents were difficult or impossible to evacuate and staff couldn't do the impossible. They simply needed more than 10 minutes

RE: Group 'I' Occupancies

2010-01-04 Thread George Church
And it might be a cold day indeed when ICC sends you to something NFPA produces in competition with ICC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker Sent: Monday, January 04, 2010 4:38 PM To:

FW: Sprinkler Helps to Save Care Home Residents

2009-12-30 Thread George Church
And to think we still have a large number of unsprinklered nursing homes here in the States...where the result wouldn't be as good as this- tey'd have shut the door and it likely would have flashed over, killing the occupant in the room of origin. After that, the fire growth would have

RE: Same sprinkler, malfunctions twice in a month!

2009-12-29 Thread George Church
Oh, all that the public needs to know is in the report- the sprinkler extinguisher sprayed water when it wasn't supposed to do that. Funny, the amount of damage is almost nil. Couple DVDs and chair legs, carpet, flooring? Adjusters would kill for such small claims on a sprkr discharge incident

RE: Flexible Couplings

2009-12-29 Thread George Church
Appreciate it- We're looking for a short Flexhead on steroids, not the dresser #38. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Tuesday, December 29, 2009 1:28 PM To:

RE: Tragic News!!

2009-12-28 Thread George Church
Horror doesn't take a holiday, and we have decades of unsprinklered housing stock that eventually will be replaced with sprinklered housing. We've finally been given the ammo, centuries after the problem started and a generation after it was available. A century after the solution of you count 13

RE: Jockey Pump spec for Vertical Turbine Fire Pump

2009-12-22 Thread George Church
Generally there's a sample spec ion most pump mfr's website. Or ask a local vendor, he'll love you for it. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim Johnston Sent: Tuesday, December 22, 2009 10:32

FW: Video of Bellefonte fire this morning....

2009-12-22 Thread George Church
Click on the link and see the latest fire to hit historic downtown Bellefonte, PA, just outside State College. After losing two 4-story historic buildings in spectacular blazes 18 months apart, then Fire Chief Tim Knisely formed the Bellefonte Fire Protection and Historical Preservation Task

RE: Video of Bellefonte fire this morning....historic buildings and areasof towns

2009-12-22 Thread George Church
A friend of mine notes they are sprinklering historic downtown Annapolis one building at a time. During the rebuild :( glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... Sent: Tuesday, December

RE: C factor in old copper pipe

2009-12-21 Thread George Church
Todd, is it possible to run a flow test at the end of the copper line to simply measure the real thing instead of degrading it? We'd had an AHJ want to degrade DI UG down to C=80 or 90, until we removed a section and showed it to him- clean as a whistle, allowed C=140 after all. glc

RE: Residential Burn Demo

2009-12-21 Thread George Church
I would hope they do, but I doubt it will bring the outrage it deserves. Residential sprinklers aren't taken for granted (obviously) so its not the same effect as if Detroit starting shipping cars without seat belts, and someone died from smashing the windshield with their face. It'll just be

RE: Ace hardware classification

2009-12-21 Thread George Church
Absolutely right. HodgePodge as in any general retail store. Thom, I know you don't want to do it, but the ONLY way to bid this is OH2 and qualify your bis as such, that you're assuming the top shelf is a CAP to signify to employees that storage can't exceed this 12' AFF mark. Cause you know most

RE: Bucket test

2009-12-21 Thread George Church
Whenever the AHJ says he wants on in 13d where the calcs don't have the same intestinal fortitude as our 13R and 13 calcs. Which begs the question- why do a bucket test if you did real calcs? glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Vote for Residential Sprinklers - NOW please!

2009-12-21 Thread George Church
Uh, did you know you can back up and vote again? A friend in Chicago noted that to me. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Tysinger Sent: Monday, December 21, 2009 4:57 PM To:

RE: Electrical Grounding

2009-12-18 Thread George Church
You could turn tables on him- Tell him to show you where it IS allowed in the code. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell Sent: Friday, December 18, 2009 12:06 PM To: AFSA Subject:

RE: storage tank drain requirement

2009-12-18 Thread George Church
I thought 22 had a drain requirement, I can't recall ever installing a tank without one. What I do recall is shaking my head why folks put drain valves on the back of a tank instead of in the pumphouse side, in the heated area, and then an ell to take it thru the wall. Sure, it's a couple feet of

RE: School fire

2009-12-17 Thread George Church
Please do update us, Tony- I can't think the 200*F heads- required in unventilated attic- are the cause. And the code DOES allow exposed CPVC in OH2 if 400 SF in light hazard building, and with spacing and elevation restrictions. glc -Original Message- From:

RE: ESFR DOES WHAT???

2009-12-17 Thread George Church
Vince, we did a job last year where our variance was approved and here's the logic train: Egress distance can be increased past 250' if heat and smoke vents are provided. So we pencil vents in. Then we provide an ESFR system so the vents aren't required, erase them. Extended egress distance in

RE: ESFR DOES WHAT???

2009-12-17 Thread George Church
I learned an interesting phrase from a former staff liason at NFPA; during committee meetings he'd observe: Since I'm not on the committee, I'm not entitled to an opinion. But if I were, I'd .. Nice caveat, he could participate without participating. And as a PE, he would otherwise BE

RE: NFPA-13 Residential Heads

2009-12-16 Thread George Church
I'd ask the EOR if you could use 13R and there's no reason you couldn't design areas outside the dwelling units to OH1- and understand not all of #13 requirements apply to areas outside the dwelling unit, but density, remote area size, etc do come over. Increase in hose streams, protection of

RE: NFPA-13 Residential Heads

2009-12-16 Thread George Church
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Wednesday, December 16, 2009 11:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: NFPA-13

RE: forward flow test problem

2009-12-14 Thread George Church
And you're trying to hit a moving target- the water supply isn't static. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Monday, December 14, 2009 1:34 PM To:

RE: tri seal gaskets

2009-12-11 Thread George Church
Before Frozen Dave became an SH wizard, he'd have chimed in here about the mini-dams that get created when roll-grooved piping has condensation puddling both in the pipe ends uphill from the groove intruding up into the bottom of the pie, as well as the water sitting in the gasket. Potential for

RE: tri seal gaskets

2009-12-11 Thread George Church
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Friday, December 11, 2009 10:18 AM To: sprinklerforum@firesprinkler.org Subject: RE: tri seal gaskets Before Frozen Dave became an SH wizard, he'd have chimed in here about the mini-dams that get created when roll-grooved piping has

RE: Pennsylvania first state to adopt one- and two-family home fire sprinkler requirement

2009-12-11 Thread George Church
help when asked, and become part of the solution instead of just bitchin and being part of the problem. Best of luck to all the others in states where you still have obstacles to overcome. Keep pushing! Write letters! Help with a local FD's side by side! Do Something! George Church Rowe Sprinkler

RE: Frozen pipe

2009-12-10 Thread George Church
Welding leads? Run around installing heat tape? Seriously, warm up the area with heaters If using salamanders cause u have to, keep FEs nearby and manned. Otherwise pull it out, set it warm area, reinstall tomorrow. And be glad for the stimulus. -Original Message- From:

RE: 13 residential sidewalls

2009-12-08 Thread George Church
Its not a criteria by which we're judged. We meet what the code outlines for us to meet. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Tuesday, December 08, 2009 10:38 AM To:

RE: Flexhead Question?

2009-12-08 Thread George Church
And as obvious as it sounds, I'd caution against a 12 offset since you'll hit ceiling wire. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Dooley Sent: Tuesday, December 08, 2009 3:00 PM To:

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-02 Thread George Church
We DO maintain annual pressure records in each sprinkler room- hanging on the main drain tag. Naturally this data is only of value when someone opening that main drain and writing down the residual pressure actually compares the result with the previous data. You're spot on that the language on

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-02 Thread George Church
/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Wednesday, December 02, 2009 5:21 AM To: sprinklerforum@firesprinkler.org Subject

RE: Domestic Demand Requirements In NFPA 13R, 2002 Edition (Handbook)

2009-12-02 Thread George Church
They can't- any more than we'll warrant that our systems will control a fire. They'll be happy to sign what they can, usually- that at the moment of the flow test, these pressures and flows were available. That's all they'll say and that's all they should say. I think it would be a good idea to

RE: QR / SR SPRINKLER SEPARATION

2009-12-01 Thread George Church
So you've just handed him the dilemma of using SR ELO's in a light hazard corridor..hope people don't die. :) Seriously, Dwayne, I'd use the ELOs up the corridor and then switch to the QR in the breakroom, assuming the breakroom is separated by a wall from the high hazard area. glc

RE: Calcs-How much margin

2009-12-01 Thread George Church
Or just qualify your proposal that storage can't exceed 12' and go OH 2 with EC heads in that 40' tall box. In April 2010 FM Global is going to slim down the selection of heads to: Storage Non-storage Residential Special They won't be differentiating between suppression and control modes, and

RE: QR / SR SPRINKLER SEPARATION

2009-12-01 Thread George Church
. If you have received this electronic mail transmission in error, please delete it from your system without copying or forwarding it, and notify the sender of the error by reply email or by calling Cherokee Fire Protection Co. at 888-347-3079 toll free. -Original Message- From: George

RE: Calcs-How much margin

2009-11-30 Thread George Church
Some day maybe I'll see if I can cut and paste what a PE around here required. I haven't been able to figure it out, it was easier to not bid their work. I do know it had nice things like: No field-installed offsets without revised calcs submitted and approved. (Know how well that works with

RE: concealed space

2009-11-25 Thread George Church
wishes for a thoroughly enjoyable thanksgiving respite. George Church Rowe Sprinkler -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David Blackwell Sent: Wednesday, November 25, 2009 9:14 AM To: sprinklerforum

RE: concealed space

2009-11-25 Thread George Church
[mailto:sprinklerforum-boun...@firesprinkler.org mailto:sprinklerforum-boun...@firesprinkler.org ] On Behalf Of George Church Sent: Wednesday, November 25, 2009 12:20 PM To: sprinklerforum@firesprinkler.org Subject: RE: concealed space And you can't use 13R under the 2006 IBC if the design team used

RE: RE: concealed space

2009-11-25 Thread George Church
-boun...@firesprinkler.org] On Behalf Of George Church Sent: Wednesday, November 25, 2009 12:20 PM To: sprinklerforum@firesprinkler.org Subject: RE: concealed space And you can't use 13R under the 2006 IBC if the design team used the sprinkler increase in order to build it, you can add a story

RE: Sprinklerforum Digest, Vol 4, Issue 16

2009-11-23 Thread George Church
http://www.sprinkleracademy.com/#/Classes/ learn velocity pressure calcs -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Miguel A. Lopez Sent: Sunday, November 22, 2009 8:04 PM To:

RE: Sprinklerforum Digest, Vol 4, Issue 16

2009-11-23 Thread George Church
Actually, I believe a newbie to the industry with a really smart father has developed a method to NOT make assumptions, but use his formula to simply plug in your values and go. I believe it will be released soon, once marketing determines how to make a buck on it. Glc -Original

RE: Storage of idle wooden pallets and hi-ex foam

2009-11-23 Thread George Church
However, when you're using stored water for 150 minute duration, cutting the density in half can save some serious money- like the job I was just finalizing when this came across, and made me give pause- did I miss a chance to lower our cost? I was thinking of popping a bladder tank in for

RE: Design Criteria

2009-11-23 Thread George Church
Well, Equivalency 1.4 gives us the ability to apply FM standards- or other alternatives- and BE IN ACCORDANCE WITH NFPA #13! Just say you're in compliance with Section 1.4 of #13, and submit the technical documentation (i.e., FM Data Sheets and any tests or other explanatory info you can find) and

RE: Design Criteria

2009-11-23 Thread George Church
Yes We subscribed to the FM Data Sheet subscription service for years in order to do just that. We've applied FM criteria on some projects since the owner may wish to engage FMG at a later date. In standard systems, simply use the 1.4 multiplier and other items where FM invokes more stringent