Owen:
What exactly do you object to if the fire official is trying to verify the
delivery of adequate fire flow? What water company or muni-utilities
department is providing the water? Have they exercised any hydrants in the
subject neighborhood in the past... I dunno, TEN years?Can
I’ve been told many times that the only time the fire dept gets to see anything
about the building is with fire sprinkler plan review so we sometimes get the
off the wall comments for things that are not in our scope. The plan reviewer
knows it is not in our scope, but the only way they can
We have before. But it was due to the loft, it fell out of IRC. (4 stories high
now)
That required it to be connected to city supply since it was an R, not a D.
Seems like yours is the domain of the civil/city for IFC fire flow requirements.
Outside your scope..
R/
Matt
-Original
We have received requests for Fire Flow verification before. It often happens
because the comments are tossed in with our plan review ("be sure the hydrants
work!")- or because they contain the word "fire"
We charge to perform them and do it under a separate agreement. We don't design
or
, PA, & TX
**NICET IV - Water-Based Systems Layout
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Steve Leyton
Sent: Thursday, May 19, 2016 10:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
Right but your comment could be misr
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Steve Leyton
Sent: Thursday, May 19, 2016 10:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
It's like sprinkler hydraulics in that the size of the piping may have to be
calculated, which
. It is not
cumulative.
Steve
Original message
From: "Hinson, Ryan" <rhin...@burnsmcd.com>
Date: 5/19/16 7:30 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
Your building sprinkler feed is just that...a sprinkler f
esprinkler.org] On
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
Steve-
Thanks for the help, I think I got it from here.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>
I have a flow graph program on Excel that you could use and read to 20 psi. It
doesn't have any capacity for calculating underground data
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Thu, May 19, 2016 at 8:55 AM, Brian Harris
:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
It's like sprinkler hydraulics in that the size of the piping may have to be
calculated, which is based on the available flow and pressure from whatever
water supply you're starting with. Usually, and I emphasize usually but not
always, a
but not if its 450
feet long.
Steve
Original message
From: Brian Harris <bhar...@bvssystemsinc.com>
Date: 5/19/16 6:48 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
Got it, thanks. I see where this particular project requires 1500 gpm @
rforum@lists.firesprinkler.org
Subject: Re: Fire Flow
So true. And I love when the specifying engineers don't research the local
amendments.
One large jurisdiction here does not allow a reduction in site fire flow for
13R systems, and only a 50% reduction for 13 systems.
I'm the bad guy when we have t
m-boun...@lists.firesprinkler.org] On
Behalf Of mphe...@aerofire.com
Sent: Thursday, May 19, 2016 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Fire Flow
In the IFC it is table B 105.2 i believe.
Mark at Aero
602 820-7894
Sent from my iPad
On May 19, 2016, at 5:56 AM, Brian Harris
0.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of mphe...@aerofire.com
Sent: Thursday, May 19, 2016 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Fire Flow
In the IFC it is table
In the IFC it is table B 105.2 i believe.
Mark at Aero
602 820-7894
Sent from my iPad
On May 19, 2016, at 5:56 AM, Brian Harris
> wrote:
Does anybody have a spreadsheet or pdf they'd care to share that is used to
calculate fire flow
erforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Brian Harris
> Sent: Thursday, May 19, 2016 9:23 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Fire Flow
>
> Craig-
> Thanks for the info.
>
> Brian Harris, CET
> BV
er.org
Subject: RE: Fire Flow
Not a problem. Fire Flow per the IFC is one area of fire protection
engineering way too often overlooked, misunderstood or just plain ignored.
Let me know if you have any other questions.
Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenvil
- 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Thursday, May 19, 2016 9:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow
Craig-
Thanks
rforum@lists.firesprinkler.org
Subject: RE: Fire Flow
You need to contact the local fire code authority and find out from them what
their approved method is for determining Fire Flow. There are more than a half
dozen methods that are used.
Once you find the method to be used, you will use the calculation metho
You need to contact the local fire code authority and find out from them what
their approved method is for determining Fire Flow. There are more than a half
dozen methods that are used.
Once you find the method to be used, you will use the calculation methodology
prescribed within.
Of the
Fire flow is a term and issue not often addressed by A/E and fire protection
engineers.
Fire Flow is a requirement within the IFC, Section 507.3 to be specific.
There are numerous methods available to use to determine Fire Flow. As the
section of Code states, Fire Flow is to be determined
@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Fire flow is a term and issue not often addressed by A/E and fire protection
engineers.
Fire Flow is a requirement within the IFC, Section 507.3 to be specific.
There are numerous methods available to use to determine Fire Flow
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Duane Johnson
Sent: Tuesday, December 22, 2015 1:48 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
To add, the fire flow is based on construction type, building height/area
IFC 2012, Appendix B
Section B105 Fire-Flow Requirements For Buildings
Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
http://www.kfiengineers.com
-Original Message-
From: Sprinklerforum
In my State, I would be able to explain it to such a customer like this:
We don't specify the exact scope of work divisions amongst the building design
team; however, the plans must comply with the applicable code requirements.
Therefore, you may need to discuss who on the design team is
Check the IBC/IFC (index... not sure what section). Fire Flow is the amount of
water required to be delivered by the fire hydrants for the FD to spray on a
burning building. The amount required is dictated by the code, but the actual
water available is determined entirely by the underground
-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ron Fletcher
Sent: Tuesday, December 22, 2015 2:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Fire Flow vs Hydraulic calc's
It's in Appendix B of IFC and is definitely in the realm
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 2:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Peter-
Much appreciated.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 1:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Definitely out of our control but I was looking for the differences between the
(2) calculations. I
Office
301-455-0010 Cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Matt Grise
Sent: Tuesday, December 22, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Check the IBC/IFC
It's in Appendix B of IFC and is definitely in the realm of A/E team. Fire
flow, hydrant spacing etc.. Is required for building permits (usually) and the
fire line size should have been determined well before a sprinkler contractor
was involved.
Sent from my iPhone
> On Dec 22, 2015, at 1:46
@lists.firesprinkler.org
Subject: Re: Fire Flow vs Hydraulic calc's
You can tell them they need a 20" line and that they might want to have the
architect verify your findings.
.
On Tue, Dec 22, 2015 at 12:17 PM, Brian Harris <bhar...@bvssystemsinc.com>
wrote:
> Ron-
> I totally
ete Schwab
Sent: Tuesday, December 22, 2015 1:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
See NFPA 13 2016 Edition A.11.1.4.2
Peter Schwab
VP of Purchasing and Engineering technologies
Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 347
--
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Fletcher
> Sent: Tuesday, December 22, 2015 2:14 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Fire Flow vs Hydraulic calc's
>
> It's in Appendix B of IFC and is definitely in the r
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Matt Grise
Sent: Tuesday, December 22, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Check the IBC/IFC (index... not sure what section). Fire Flow is the amount
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
See NFPA 13 2016 Edition A.11.1.4.2
Peter Schwab
VP of Purchasing and Engineering technologies
Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761
Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax
Subject: RE: Fire Flow vs Hydraulic calc's
Brian
A.11.1.4.2 Appropriate area/density, other design criteria, and water supply
requirements should be based on scientifically based engineering analyses that
can include submitted fire testing, calculations, or results from appropriate
computational
If you're talking about the fire flows referenced in the IFC, Appendix B, this
seems to be an AHJ or IU call. For the most part when the building is fully
sprinklered only the sprinkler system demand and hose stream demands are used
for water tank sizing. I've not had one AHJ or IU apply the
The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property. My question is (and no fire marshal
to ask today),is the sprinkler demand included or need to be added?
This tank supplies all fire water needs (no jokes-I know what you're
all thinking) for this
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property. My question is (and no fire marshal
to ask today),is the sprinkler demand included or need to be added?
This tank supplies all fire water needs
Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Thursday, September 03, 2009 12:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
, Inc.
(209)334-9119
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim Johnston
Sent: Thursday, September 03, 2009 1:11 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow
Ron,
Is this in a rural
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Thursday, September 03, 2009 12:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property. My
I don't have a quick answer, but out of curiosity, how far does the FD need to
go to get another water source?
BTW, the hose allowance in the sprinkler design must surely be part of the
fireflow.
Dave
David A. de Vries, P.E., CSP
Firetech Engineering Incorporated
--- On Thu, 9/3/09,
]
Sent: Thursday, September 03, 2009 12:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property. My question is (and no fire marshal
to ask today),is the sprinkler demand included or need
Far. And yes the fire flow accommodates the demand for both. I'm
trying to figure how much storage is needed.
On Thu, Sep 3, 2009 at 1:30 PM, David de Vriesddevr...@firetecheng.net wrote:
I don't have a quick answer, but out of curiosity, how far does the FD need
to go to get another water
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, September 03, 2009 4:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
Jim,
Let's say semi-rural. The fire department is coming but all the water, for them
and the sprinklers is from the tank. The actual
...@inlandfireprotection.com
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Thursday, September 03, 2009 12:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property
...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, September 03, 2009 2:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
Far. And yes the fire flow accommodates the demand for both. I'm trying to
figure how much storage is needed
] On Behalf Of Ron Greenman
Sent: Thursday, September 03, 2009 1:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow
Far. And yes the fire flow accommodates the demand for both. I'm
trying to figure how much storage is needed.
On Thu, Sep 3, 2009 at 1:30 PM, David de Vriesddevr
: Thursday, September 03, 2009 4:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow
Ok so let's just remember that if you have insufficient Fire Flow per the I
codes, one of the alternatives is to fire sprinkler the property. So in the
I-codes Sprinkler = Reduced fire flow
Subject: RE: Fire Flow
NFPA 13 2002 Edition 11.2.3.1.3; An allowance for inside and outside hose
shall not be required where the tanks supply sprinklers only. Since the tank
supplies both site fire hydrant and fire sprinklers, it needs to accommodate
both the site and sprinklers. The questions I
://www.ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregg Fontes
Sent: Thursday, September 03, 2009 5:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow
NFPA 13 2002 Edition 11.2.3.1.3
Sent: Thursday, July 24, 2008 3:53 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
The other thing to remember about the ISO Fire Flows is that they limit the
maximum flow to 3500 Gpm @ 20 Psi per hyd.
To most of you this will sound like water from heaven. Up here
Don't give them any ideas.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Thursday, July 24, 2008 4:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Flow Calculation
I recently read a spec that required the sprinkler
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
To REALLY make things interesting, the ISO method of calculation is for
an unsprinklered building only.
ISO defines the Needed Fire Flow for a sprinklered building to be the
sprinkler system demand plus the appropriately
Subject: RE: Fire Flow Calculation
The other thing to remember about the ISO Fire Flows is that they limit the
maximum flow to 3500 Gpm @ 20 Psi per hyd.
To most of you this will sound like water from heaven. Up here in the
hill's, we often have 3500 @ 80, and lose the ability to flatten
Ron,
Just a few questions to stimulate the ole thought processes this morning ;-)
(1) What fire flow calculation method are you required (or allowed) to utilize
in the jurisdiction you are referencing?
(2) Have you calculated the effective area based on the allowed
compartmentalization of the
gpm to the AHJ.
Thanks to everyone for your input.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Thursday, July 24, 2008 7:22 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow
:37 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
I think I have tried the ISO method before and unless I did something
wrong (easily) the fire flows I ended up with for large buildings were
greater than those in Appendix B.
At the very least I will need a lot more
Vance
Sent: Thursday, July 24, 2008 8:22 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
The reason for the ISO method being more atractive is that ISO allows the
Effective Area to be calculated utilizing 2hr fire separations for
compartmentalization.
In simpler words, you
: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Thursday, July 24, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
Never ceases to amaze me what they think WE should be expert at, yet we
have township inspectors looking over our work
-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, July 24, 2008 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
Likewise when licensed fire protection contractors get caught attesting
that
the vane type flow switch
24, 2008 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
Likewise when licensed fire protection contractors get caught attesting
that
the vane type flow switch operates properly yet no ITC exists. Lots of
red
faces this morning, but not to worry the fire
Tables B and C of the IFC ( I think) list the flows. An intersting
question arises..., if it is not fully sprinkled... I believe you do not
get the nice reduction?.. Is this what you are looking for ?
R/
Matt
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On
Fire flow from hydrants, standpipes, sprinklers - what?
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, July 23, 2008 4:36 PM
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Calculation
Looking for help to determine
]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Wednesday, July 23, 2008 1:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
Tables B and C of the IFC ( I think) list the flows. An intersting
question arises..., if it is not fully sprinkled... I believe you do
Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 5:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
It's for fire flow from hydrants. I guess I'm wondering if we can
pro-rate the unsprinklered
I was afraid of that. So it will be 6000 gpm.
Thanks for the help.
Ron
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, July 23, 2008 2:17 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
Nope
PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, July 23, 2008 3:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
I was afraid of that. So it will be 6000 gpm.
Thanks for the help.
Ron
-Original Message-
From: [EMAIL PROTECTED
That's a good idea but with my luck there will be asbestos above the
ceilings.
Ron
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, July 23, 2008 2:32 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
23, 2008 3:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
That's a good idea but with my luck there will be asbestos above the
ceilings.
Ron
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, July
You can't get 4800-gpm at 20-psi with that flow test, no matter what you do
(the best you can do is 4018-gpm); and you can't get 4800-gpm through that
fire pump, no matter what you do. The city wants their Needed Fire Flow for
the building and there are several methods to figure the NFF but most
If the building is fully sprinklered, I believe IFC allows up to a 75%
reduction of the required fire flow?
R/
Matt
Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
-
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Hasenmyer
Sent: Wednesday, October 03, 2007 8:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow requirements
You can't get 4800-gpm at 20-psi with that flow
I deal with this problem everyday here in Phoenix. Table B105.1 list the
required fire flows based on total square feet of the largest building
on a site. B105.2 Exception allows up to a 50% reduction in fire flow
for buildings sprinklered in accordance with 903. It doesn't sound like
the AHJ has
PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, October 03, 2007 8:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow requirements
I deal with this problem everyday here in Phoenix. Table B105.1 list the
required fire flows based on total square feet of the largest building
03, 2007 8:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow requirements
I deal with this problem everyday here in Phoenix. Table B105.1 list the
required fire flows based on total square feet of the largest building
on a site. B105.2 Exception allows up to a 50% reduction in fire
address.
- Original Message -
From: Bobby Gillett [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Wednesday, October 03, 2007 10:02 AM
Subject: RE: Fire Flow requirements
The project is using 2003 IBC and I don't see the chart or exception in
there. Is this new to 2006 IBC
to fight, Ground Zero?
Ray Schmid
Koffel Associates
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Wednesday, October 03, 2007 12:24 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow requirements
Still haven't heard from
@firesprinkler.org
Subject: RE: Fire Flow requirements
They may want to save everyone the trouble and just ban non-sprinklered
buildings. I don't know of too many municipalities that can deliver
8,000 gpm even at 20 psi (or 5,600 gpm for that matter) That's an awful
lot of water and seems pretty
Not specifically. The IFC states in Section 508 FIRE PROTECTION WATER
SUPPLIES, 508.3 Fire Flow: Fire flow requirements for buildings or
portions of buildings and facilities shall be determined by an approved
method.
Typical weasel-word stuff, interpret as you wish. Has the local Fire
Marshal
IFC
From: Pete Schwab [EMAIL PROTECTED]
Reply-To: sprinklerforum@firesprinkler.org
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Requirements
Date: Wed, 25 Jul 2007 09:33:02 -0400
Forum
Is there any code language or requirements that a private supply main
for a building/complex be
No there is not. As a previous post indicated, the language of 508.3
states that fire flow shall be determined by an approved method. If
you go to Appendix B, Fire Flow for Buildings, you will find the
required minimum flow rates and durations, based on building type and
area (but NOT based on
Steve's description is how we apply these requirements in Seattle.
Think a bit about the scenario, if a fire is to the point that the hose streams
are using the volume required for fire flow, (1,500 - 4,000 gpm) the
sprinklers obviously did not work very well in the first place, might as
, 2007 10:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Requirements
Steve's description is how we apply these requirements in Seattle.
Think a bit about the scenario, if a fire is to the point that the hose
streams are using the volume required for fire flow, (1,500 - 4,000