RE: CPVC Seismic

2017-09-18 Thread MFP Design, LLC
Really no different. I doubt you will find longitudinal bracing listed for cpvc. You will have to put a short branch (same size as main) perpendicular to the main and brace that with a lateral brace to act as your longitudinal brace on the main. From: Sprinklerforum

RE: Riser Details

2017-10-06 Thread MFP Design, LLC
Do you have a mentor working with you? If you really have no idea, I would suggest you find a local mentor to help you. But in the meantime, go drive to the nearest site and check out their riser. The configurations can vary per geographical region. From: Sprinklerforum

RE: Pipe Schedule System

2017-10-06 Thread MFP Design, LLC
I have to agree with Matt on this. Give the assessment of what is required to work and meet the requirements of the standards and codes. Sadly, you can never take liability out of the question. If you know it is wrong, you have to be willing to sleep with that decision every night because

RE: Calcs and tenant improvements

2017-10-06 Thread MFP Design, LLC
al, that is jurisdiction specific. We have PE on staff and seal in jurisdictions that require. This has just been something that has been popping up more and more. It was very rare in the past. We maybe calculated 1:100. Now I am seeing 3:5 requiring it for the jurisdictions I deal with. Travi

RE: Calcs and tenant improvements

2017-10-06 Thread MFP Design, LLC
uiring it for the jurisdictions I deal with. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: <https://www.facebook.com/pages/MFP-Design-LLC/92218417692> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDe

SIN question

2017-10-03 Thread MFP Design, LLC
? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

Marriott Module 14

2017-09-08 Thread MFP Design, LLC
. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Marriott Module 14

2017-09-08 Thread MFP Design, LLC
Got it already. Thanks to everyone!! From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Friday, September 8, 2017 10:32 AM To: sprinklerforum@lists.firesprinkler.org Subject: Marriott Module 14 Does anyone have a copy of the 2015

RE: Obstructed Construction Clarification

2017-10-09 Thread MFP Design, LLC
I have been required to have the “flutes” packed with mineral wool in order to use panel construction in circumstances like you indicate. We have used beam and girder without the packing when the spacing permits. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298

RE: Schedule 10 vs Schedule 40 pipe

2017-10-04 Thread MFP Design, LLC
returned hundred fold every year with things I have learned and gained as an AFSA member. Join up today!! Ok.. back to your regularly scheduled programming… Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email

RE: Schedule 10 vs Schedule 40 pipe

2017-10-04 Thread MFP Design, LLC
No…not a shot at anyone. Lol!! Just the usual plug for membership. I’m sure you realize the crazy value we get as design members. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Paulsen Sent: Wednesday, October 4, 2017 3:14 PM To:

RE: Schedule 10 vs Schedule 40 pipe

2017-10-04 Thread MFP Design, LLC
Of MFP Design, LLC Sent: Wednesday, October 4, 2017 6:15 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Schedule 10 vs Schedule 40 pipe No…not a shot at anyone. Lol!! Just the usual plug for membership. I’m sure you realize the

One Last AFSA plug

2017-10-04 Thread MFP Design, LLC
teaching classes, it is still worth it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fww

RE: Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread MFP Design, LLC
have to be listed QR. They have to be FR. Basically, they need a 3mm bulb. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread MFP Design, LLC
Yes. When the storage got brought into 13, it used to be Curve 1-5 which happened to align with the classic hazard curves. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark Sornsin [FAR] Sent: Wednesday, October 18, 2017 11:31 AM To:

Occupant load

2017-10-23 Thread MFP Design, LLC
Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d

RE: Occupant load

2017-10-23 Thread MFP Design, LLC
@lists.firesprinkler.org Subject: Re: Occupant load That's new and interesting and not required in 13. No, I haven't heard of that one. On Oct 23, 2017 8:42 PM, "MFP Design, LLC" <tm...@mfpdesign.com <mailto:tm...@mfpdesign.com> > wrote: Has anyone had to

RE: Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread MFP Design, LLC
Is this a solid mezzanine? I guess that I see adjacent in this case meaning at the same level.. basically you can’t have ESFR sprinklers adjacent to SR sprinklers at the same roof level. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: NFPA 13 on iphone

2017-11-29 Thread MFP Design, LLC
To solve such issues, I purchase the standards in PDF format. I then store them in a dropbox folder so I can access any time from the phone or computer. Maybe that will help you. It doesn't answer your direct question, but does offer an alternative. Travis Mack, SET MFP Design, LLC

RE: [EXTERNAL] Re: Saw-Tooth Ceilings

2017-12-03 Thread MFP Design, LLC
No, you don’t ignore the obstruction. I agree with that. I was just pointing out that SxL is not always the same for spacing and calculations. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.

RE: [EXTERNAL] Re: Saw-Tooth Ceilings

2017-12-03 Thread MFP Design, LLC
Not necessarily. Remember the generic phrase: Space on the slope, calc on the flat. So, you may be at 130 sq ft on the slope, but if it translates to 110 sq ft on the flat, then you calc for 110 sq ft. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf

Informal Interps

2017-12-19 Thread MFP Design, LLC
knowing as the EOR. However, having the backing of the AFSA to our position, the EOR backed off of his incorrect interpretations and is going to be working on re-designing the issue in question. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: Informal Interps

2017-12-19 Thread MFP Design, LLC
inion only, as a member of the NFPA 13 Technical Committee, and do not represent an official interpretation of the NFPA 13 standard. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, December 19, 2017 10:40 AM To: sprinklerforum

RE: [EXTERNAL] Multiple Pumps

2017-12-19 Thread MFP Design, LLC
I’ve had some large demand systems….5000 gpm and more. They always had specified (3) 2500 gpm pumps for the 5000 gpm systems. I had one 9000 gpm system that had (4) 3000 gpm pumps. The idea was that if any one pump was done, the system would still be maintained with adequate pumping

RE: FDC sizing on wet automatic standpipes

2017-11-17 Thread MFP Design, LLC
to use 4”, but you will still need 4 inlets. I think that seems quite odd and would probably try to run it as 6” as a good practice. However, I can’t see anything requiring the size of the piping to be any minimum. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298

RE: Standpipe Pressure Question.

2017-11-01 Thread MFP Design, LLC
Standpipe only has to be Automatic for high rise, unless the area has adopted an amended code requiring it to be automatic. So, the question still sits, is it a high rise building? If not, then is there the option to make it manual wet? From: Sprinklerforum

RE: Dry automatic standpipe without a pump

2017-12-05 Thread MFP Design, LLC
Definitely don't let the past description or even system get in the way. It is what it is. If the original is wrong, the owner can go back and fix it. But there is no reason to continue an error just because it was done that way in the past. Those are the most dangerous words in this industry:

RE: [EXTERNAL] RE: Dry automatic standpipe without a pump

2017-12-05 Thread MFP Design, LLC
desires. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

Roof Crickets

2017-12-06 Thread MFP Design, LLC
they communicate directly with the main attic. However, I can't find anything that would permit them to be omitted. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: Underground Main Between 2 Attached Building Areas

2017-12-11 Thread MFP Design, LLC
, if there is an underground leak, you don’t have to take out the entire building. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook

RE: [EXTERNAL] RE: Protection under bleachers in a Gymnasium

2017-12-12 Thread MFP Design, LLC
f248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.high

RE: Occupant load

2017-10-24 Thread MFP Design, LLC
Still only half correct. I still wait for the day when the plan is a dot on a map and says sprinkler guy to provide system and all of building. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http

RE: Underground Main

2017-10-24 Thread MFP Design, LLC
h flow 1500 and pressure of 100. I hope that clears it up. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/

RE: Underground Main

2017-10-24 Thread MFP Design, LLC
as simple of a calc as you can get if it is a dead end main. If you need something for your computer software, just go with flow 1500 and pressure of 100. I hope that clears it up. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Underground Main

2017-10-24 Thread MFP Design, LLC
o does the flow need to be increased to 2000 do to there being two hydrants? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, October 24, 2017 4:04 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprin

RE: Underground Main

2017-10-24 Thread MFP Design, LLC
You need to know the method of determining fire flow in your jurisdiction. Once you know that, determine the fire flow and the number of hydrants req'd to be used to get that flow. Then, just simple hazen Williams formulae. You will have starting flow and pressure. Plug and chug to prove it.

RE: [EXTERNAL] RE: Underground Main

2017-10-24 Thread MFP Design, LLC
entral Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 <mailto:kmontgom...@aerofire.com> kmontgom...@aerofire.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, October 24, 2017 1:30 PM To

RE: [EXTERNAL] RE: Underground Main

2017-10-24 Thread MFP Design, LLC
; kmontgom...@aerofire.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, October 24, 2017 1:30 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: [EXTERNAL

RE: Misc Rack Storage

2018-05-17 Thread MFP Design, LLC
When you have mixed criteria areas, you need to extend the higher density into the lower density area for 15’. Reference NFPA 13: 12.3 for that requirement. Also, don’t forget the issue of complying with 23.4.4.1.1.4. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ

RE: Water Delivery Times

2018-05-18 Thread MFP Design, LLC
It is from the time the head opens as the way I understand it and had to meet requirements of. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Ground Storage tank

2018-06-13 Thread MFP Design, LLC
It sounds like you are indicating you want to use a "brake tank." As long as you put an automatic fill valve on the tank, you can use the city supply to help reduce the quantity of stored water. You may want to check NFPA 22 for this. Travis Mack, SET MFP Design, LLC 3356 E

RE: Ceiling Grids and Flex Drops

2018-05-30 Thread MFP Design, LLC
Tell him they are UL Listed for use in fire sprinkler systems. He needs to prove that they can't be used. Call Victaulic. I would imagine they can get you something. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email

RE: ESFR closer than 8'

2018-05-30 Thread MFP Design, LLC
My understanding is the same as Don stated. It is not skipping or cold soldering. It is too many sprinklers opening. The baffle or curtain will do little, if anything, to alleviate that. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: Ceiling Grids and Flex Drops

2018-05-30 Thread MFP Design, LLC
What was the final resolution?? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
for storage sprinklers. So, even though the 11.2 is just a standard spray sprinkler, you must adhere to all of the storage sprinkler obstruction and spacing criteria of the appropriate FM Datasheet. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
ESFR are not spray sprinklers and can not be interchanged to meet a density/area curve. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
I always try to contact the FM reviewer and ask for the table where they are getting the info in their datasheets. I then put that table on the drawings so there is no question as to where the criteria was derived. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2F

RE: % open

2018-06-25 Thread MFP Design, LLC
Yes. That is exactly it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.

% open

2018-06-25 Thread MFP Design, LLC
, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
Matt: I think Craig is dealing with some one that thinks if the calcs say you only “need” 40 psi at the base of riser, then that is all that the water supply will deliver. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
We all make mistakes and things happen. But, there does appear to be a huge gap in understanding some times. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
minimums. You can run supply calcs to determine what pressures and flows you can expect with the full water supply discharging. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> em

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightai

RE: [EXTERNAL] RE: % open

2018-06-25 Thread MFP Design, LLC
This is all steel construction. The exterior projection overhang is steel construction and the new add on to the clubhouse that this projects from is also steel construction. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: S & L Rule

2017-12-21 Thread MFP Design, LLC
ways done it. I just see the reasoning behind the question. Does the answer change if you have a girder instead of a beam? Why or why not? Merry Christmas to all and to all a good night! Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-4

RE: S & L Rule

2017-12-21 Thread MFP Design, LLC
sprinklers to a line. It is generally more costly to add extra lines. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook

RE: Calculation of sprinklers under soffits

2018-01-24 Thread MFP Design, LLC
them to K4.2 or 2.8 if you are in a light hazard space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: 3-Hour Rated Walls

2018-02-02 Thread MFP Design, LLC
Make sure you can get a sleeve/caulk combo to give the 3 hour rating. That may be a challenge to find. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Datasheet NFPA

2018-02-05 Thread MFP Design, LLC
www.nfpa.org <http://www.nfpa.org> They accept many different forms of payment. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com &

RE: Sprinkler in vertical duct

2018-02-07 Thread MFP Design, LLC
Dig into the areas of 13 about that. I don’t have the reference off hand, but you have provisions to use sprinklers in different orientations for the exhaust duct. So, just put a pendent sprinkler in the horizontal position. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
not be able to deliver the needed water, but that is something different. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.ou

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
I didn't even read that. NFPA 13 uses nominal k-factors. There is no difference in a K17 and K16.8. Look in Chapter 6. You will see anything with a range of 16.0-17.6 is to be calculated at k16.8 Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
I believe you are going to be out of luck. As far as I know, Tyco is the only one that makes one. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Sprinklerforum Digest, Vol 59, Issue 4

2018-02-13 Thread MFP Design, LLC
, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com

RE: Institutional sprinklers in 13R

2018-02-07 Thread MFP Design, LLC
3. Can you justify the sleeping areas are the "dwelling units" and the corridors / kitchens / living rooms are the areas "outside the dwelling unit" so that you can apply 13R? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 4

CFC 2016

2018-02-21 Thread MFP Design, LLC
sprinkler based on calculations * Edition of NFPA 13 We have to provide a copy of this sign on our plans. Additionally, we have to provide a copy of the General Information Sign on the plans. Things in CA get more and more unusual every year. Travis Mack, SET MFP Design, LLC

RE: CFC 2016

2018-02-21 Thread MFP Design, LLC
than Bitcoin in 2017. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign

RE: QR/SR Sprinklers

2018-02-15 Thread MFP Design, LLC
that you have to use a listed SR K5.6 sprinkler in the space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?ur

RE: [EXTERNAL] Re: ESFR Heads in Concrete Tee's

2018-02-16 Thread MFP Design, LLC
I think the issue is that ESFR sprinklers can’t be less than 8’. You can do <6’ with SSU/P sprinklers as the standard references baffles in those instances. ESFR is a different animal. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-

RE: inrack sprinkler question

2018-02-23 Thread MFP Design, LLC
from 16.2.1.4.3.1 to the demand calculations for the ceiling sprinklers and balance to the higher of the two pressure demands to ensure that the water supply can handle the simultaneous operation of ceiling and in-rack sprinklers." Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert

RE: HVLS Fan clearance

2018-07-27 Thread MFP Design, LLC
Maybe some one could do some model simulation on the effects of the fans, clearances ≤36”, sprinkler activation time and maybe a few other variables. I don’t know how one models the obstructions of the fan blades, but it may be possible. Travis Mack, SET MFP Design, LLC 3356 E Vallejo

System area limitations

2018-07-31 Thread MFP Design, LLC
vis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f1

RE: [EXTERNAL] System area limitations

2018-07-31 Thread MFP Design, LLC
Yes. I checked. There is nothing like that. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: System area limitations

2018-07-31 Thread MFP Design, LLC
I can’t tell you how many times I’ve wanted to send a bill to a plan reviewer titled “Education Expenses” Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

RE: System area limitations

2018-07-31 Thread MFP Design, LLC
ion. This guy is a “senior fire protection consultant” doing the review. There have been several comments along these lines. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpd

RE: definition of public space

2018-07-25 Thread MFP Design, LLC
. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Paint Booths

2018-07-25 Thread MFP Design, LLC
Don't forget to apply NFPA 13: (2016) 23.4.4.2.4 and 23.4.4.2.5. That can make some of these smaller areas be a bit of an issue. The same thing is also in the 2013 edition as well. It is 23.4.4.1.1.4 and 23.4.4.1.1.5 in the 2013 edition. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct

Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
way lately. Doing that has differing slopes and the lines would intersect. The theoretical reduction could actually have a higher pressure at a given flow with #2 since it is a flatter curve. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
There are many ways to address this. Some AHJs want us to reduce the curve off the top. Others want us to keep it as measured and maintain a minimum margin. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
In this example… Apply a 10% reduction to the measured flow test results. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
Yes. It would be at the horizon for sure  Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
Your description of accessible by more than one dwelling unit is exactly the way I view it. But, I got shot down by the AHJ. Their response was: “What if some one propped open a door?” Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
to the floor joists. We can be up in the joist space running parallel. So, CPVC or steel? What is the forum consensus? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: Baffle for fire sprinkler system

2018-08-13 Thread MFP Design, LLC
Those are useless. There is no criteria because they are not permitted. If you need a water shield, use a listed sprinkler with water shield. If you need a “heat collector”, you are out of luck. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d

RE: NFPA 13 Closet Definition

2018-08-20 Thread MFP Design, LLC
understanding. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: FM APPROVAL

2018-08-25 Thread MFP Design, LLC
https://www.approvalguide.com/CC_host/pages/public/custom/FM/login.cfm You just have to register Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Flange Spacers?

2018-07-09 Thread MFP Design, LLC
It is just a short “main” with a size on size welded outlet. Don’t we do that all the time? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

Duct Sox / ESFR

2018-03-13 Thread MFP Design, LLC
Has anyone come across the duct sox and ESFR protection? How do you handle these? I intend to put a sprinkler under the duct as normally required. But, these somewhat vanish when the HVAC system is off. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271

RE: stages

2018-03-15 Thread MFP Design, LLC
Do you run a separate standpipe system for the hose valves, or come off the overhead? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692

stages

2018-03-15 Thread MFP Design, LLC
off the overhead system and just add 50 gpm per hose valve for your inside hose requirements? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Residential Sprinklers

2018-03-06 Thread MFP Design, LLC
for area of sprinkler in 13R. So, you may have to choose the larger k factor residential sprinklers. We typically do a 4.9k pendent, but you may have to go to the larger ones depending on your requirements. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax

RE: Expansion Joint

2018-04-11 Thread MFP Design, LLC
Yes. If you are in 9.3, you are doing seismic bracing. If you are Seismic Design Cat A or B, typically you are not going to do seismic and 9.3 with it's sub chapters would not apply. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

Floor Assemblies

2018-04-05 Thread MFP Design, LLC
ce with 8.15.1.2.6. It just seemed strange that there wouldn't be some other exception to eliminate sprinklers in that space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...

RE: Assembly or Not?

2018-04-20 Thread MFP Design, LLC
tion." Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDes

RE: Strainer ahead of fire pump

2018-04-24 Thread MFP Design, LLC
It’s not required but is permitted. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpd

RE: Perpendicular to Slope / Attic

2018-04-17 Thread MFP Design, LLC
Yes. It is across the joist. 5' is a minimum. You can exceed it as long as your spacing limits are adhered to. Maybe 5' from one side and 6' from another to get away from the hip? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: PVC drain line

2018-03-30 Thread MFP Design, LLC
. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: PVC drain line

2018-03-30 Thread MFP Design, LLC
for the drain lines. It is highly impractical from a cost perspective. Check in A3.2.1 in the 2016 NFPA 13 handbook if you have it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi