RE: Conveyor Protection

2018-05-14 Thread Jeff Hewitt
Bob,

Look at NFPA 15 for conveyor protection for water spray systems, this may 
reinforce what you are looking at, perhaps substitute sprinklers instead of 
water spray

Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

[cid:image001.png@01D3EB87.1D50C020]
American Fire
www.american-fire.com<http://www.american-fire.com>
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

  
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bob
Sent: Monday, May 14, 2018 12:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Conveyor Protection

I'm looking at protecting an exterior conveyor used for crushed rock.
The insurance provider for this project has provided the following design 
guidance, "provide sprinkler coverage".
NFPA 120 seems to be the only standard that provides conveyor protection 
criteria, so I'm using that for my guidance.
There will be a .25 density with nozzles 8' o.c.   NFPA 120 8.4.6.3.2(1) 
states, "shall be installed in accordance with NFPA 13 as far as practical".
With that said, there is no guidance for design area.  Looking at 13, for a 
density of .25 there is no area given.
Would it be appropriate to use 1500 sf + 30% for preaction or should it be 2000 
sf + 30%.
Then, can the area be extrapolated to use the 1.2 x area for length of remote 
area.
There will be two nozzles every 8', one upper, one lower.  This would than 
allow for about a 53' design area (or 61' for the larger area).


Thank you,

Bob Knight, CET III
208-318-3057
[FBK-LOGO-SMALL]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Informal Interps

2017-12-19 Thread Jeff Hewitt
Good Job Travis.

Merry Christmas!!

Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

  [cid:image003.png@01D378B7.4650E010]
American Fire Protection, LLC
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

  
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of MFP Design, LLC
Sent: Tuesday, December 19, 2017 10:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Informal Interps

Merry Christmas all.  This is just another plug as to the many benefits of 
being an AFSA member.  I was having an issue with an EOR on a project.  The 
informal interpretation let them see things as we had believed was correct.  
Often, the sprinkler guy is seen as being self-serving and not as all knowing 
as the EOR.  However, having the backing of the AFSA to our position, the EOR 
backed off of his incorrect interpretations and is going to be working on 
re-designing the issue in question.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 38" wide soffit along wall

2017-02-22 Thread Jeff Hewitt
See figure A*.6.5.1.2 from NFPA 13, 2016

[cid:image007.png@01D28CE9.3EDD6110]





Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

  [cid:image008.png@01D28CE9.3EDD6110]
American Fire Protection, LLC
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

  
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Gregory Lindholm
Sent: Wednesday, February 22, 2017 8:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: 38" wide soffit along wall


I thought I knew the answer to this one, but now having second thoughts



21'-6" to roof deck, Light Hazard, 38" wide soffit along a wall @ 8'-2" above 
the floor.



Do we need sprinklers under the soffit?



1st thought was no, because it is less than 48" wide, but then looking @ NFPA 
#13 - 2016, 8.6.5.1 and 8.6.5.2, it looks like we "will need" heads under the 
soffit.



It is not like something 38" wide sitting out in the middle of a room where a 
pattern could develop around the obstruction from different areas. The edge of 
this soffit goes to the roof deck, so no pattern can develop around it.



Thoughts?


Greg Lindholm
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: HDPE Plastic Bin Box Storage

2016-12-08 Thread Jeff Hewitt
John,

I'm writing off on the forum because I don't want to stir up a hornets nest.

Isn't this an engineering decision, not a NICET SET decision?

I'm just saying, why would you want to take that liability as a NICET SET, and 
also potentially violate your NICET Certification by practicing engineering.

Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

  [cid:image005.png@01D2513A.37965DC0]
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

  
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 9:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: HDPE Plastic Bin Box Storage

Hello All!

I am working with a truck parts supplier who has moved into an existing 
warehouse and I am providing a design study to them on the existing system.

Pertinent Facts:

6"x6"x2" Grid with K-8.0 Upright Heads fed by a pump. Pipe is at 25' AFF.
Metal truck parts storage in HDPE Plastic Bin Boxes stored no higher than 10'
Existing system with 500 GPM hose calcs to .60 GPM / 3,000.
Tokyo Mutual Insurance

Personally I think the system provides adequate protection for the storage 
configuration. In fact it is MORE than sufficient according to NFPA 13, Ch 14.  
However the insurance company is maintaining that the plastic bin storage boxes 
represent an additional hazard. This is a new experience for me. My contention 
is that the Bin Boxes, even though they are made of HDPE Plastic, do not 
represent an increase to the commodity classification because of their higher 
flash point. (which is information I can't seem to find right now)

Is there a fire test out there that indicates these bin boxes represent an 
increased hazard?

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Calculating extended coverage

2016-07-13 Thread Jeff Hewitt
Timothy,

Small room rule cannot exceed 225-sq.ft. per head.  16 x 16 is 256-sq.ft.

per NFPA 13, for small rooms, the heads are averaged,

“Where a small room, as defined in 3.3.22, is considered, the area of sprinkler 
coverage
is calculated as the area of the room divided by the number of sprinklers in 
that room.”



Also, a  4 head calc. is not correct for the 900-sq.ft. area.

For quick response area reduction, i.e. 900-sq.ft. area, from NFPA 13,

“11.2.3.2.3.2 The number of sprinklers in the design area shall never be less 
than five.”

For extended coverage heads, from NFPA 13,

“11.2.3.2.2.3 For extended coverage sprinklers, the minimum design area shall 
be that corresponding
to the hazard in Figure 11.2.3.1.1 or the area protected by five sprinklers, 
whichever is greater.”


Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

  [cid:image002.png@01D1DD1D.D0067810]
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

  
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Timothy W Goins
Sent: Wednesday, July 13, 2016 2:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Calculating extended coverage

Use the small room rule where the head is allowed to be 9' from one wall and 
calc as if it were a 16 x 16. Less pressure and water overages. 4 head calc for 
900 sqft.

"For I am not ashamed of the gospel, because it is God's power for salvation to 
everyone who believes..." HCS Romans 1:16
"Therefore having overlooked the times of ignorance, God is now declaring to 
men that all people everywhere should repent,..." NASB Acts 17:30

On Jul 13, 2016, at 9:50 AM, Jay Stough 
<jaycs7...@gmail.com<mailto:jaycs7...@gmail.com>> wrote:
I have a nursing care facility that I am trying to calc.  Must be 13 (2007) 
light.  Can not use room design or residential method per state AHJ.  The 
building is shaped like an upper case H with the bottom legs cut off.  There 
are 4 rooms on one side of the corridor and 3 rooms on the other side of the 
corridor in each upper leg that use extended coverage sprinkler in each room.  
Also 1 standard spray sprinkler in a closet and one standard spray sprinkler in 
a bathroom in each room.  Sprinklers in the corridor are standard spray also.  
Since I am using extended coverage sprinklers, I need to calculate 5 minimum.  
The sprinklers cover 16'3 X 14', so need to calc at the 18' X 18' rate.  
22.4.6.2 allows me in "rooms like closets, washrooms and similar small 
compartments requiring only one sprinkler shall be permitted to be omitted from 
calculations within the area of application".   Can I calculate 6 extended 
coverage sprinklers, without the corridor or "small rooms or compartments" for 
my 1500 sq ft?  Or should I calc 5 extended coverage and the hallway sprinklers 
in the 1500 sq ft?

Jay Stough
NICET IV LAYOUT
NICET III ITM
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: "Self Storage" building design

2015-09-14 Thread Jeff Hewitt

OH II Minimum, perhaps more.  Class IV Commodities on racks needs EH-I.  
Extensive shielding of combustibles would require EH-II.

OH I only protects Class I and Class II Commodities, regardless of 8-ft. 
height.  Safe to assume there will be more than just Class I and Class II 
Commodities inside that storage unit.


Jeff Hewitt, PE, SET, PMSFPE
Corporate Engineer

   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)



Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Lamar Vaughn
Sent: Monday, September 14, 2015 3:52 PM
To: Sprinkler Forum
Subject: Re: "Self Storage" building design

The buldings of this nature I have delt with had a wire mesh ceiling at 8'-0" 
which limited the storage height to less than 8 ft. Hence O.H. I. If storage is 
over 8ft., then O.H.II .

On Mon, Sep 14, 2015 at 4:38 PM, <wmens...@comcast.net> wrote:

> I have a 3-story "Self Storage" building divided into various sized 
> rental units.
> Maximum storage height is about 10' or less.
>
> What design criteria is being used for this type of occupancy?
>
> Thanks
>
>
>
> Bill Menster
> WFM Consulting Inc.
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://cp.mcafee.com/d/5fHCN8i6hESyMMCCUOYqen3tPqdQT4Qm4S4jqdQT4QnQQnP
> qdQT4Qm4S4PqdQT4Qn1Or1Ih9-oBeoaRnUOJI7phZqdp_qsGMB2TbCZl-cHr1SkvmzmvSD
> aI9gJOVJVZBAsW-_R-vuosLRXBQShPT8FCzCWrfbnjIyyHtNfBgY-F6lK1FJ4SCrhWWl6O
> 5bhAgYTsS03fBitetB7WbhB0GvYu00UvaAVgtHM2phqcE5j_yXmbqFtSkvEJ6k2F_NU02r
> EJ6k2F_NtH5JkKgGT2TQ1hYGjFPIE_hqcE5j_zM04SMyOUr1vF6y0Qh37DKCy0oDmeAvd4
> hEw8dOfgB0yq84fF8z0SOMrTPPD
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://cp.mcafee.com/d/1jWVIgdEIc9FKcL6zBMTsSztdNd5xdx4SztdNd5Zd5YSztdNd5xdxcSztdNd5MsCMr4ivC9jC2Jl-cHr1SkvmzmvSDaI9gJOVLlvzaSMtB7RERDZFOH2kbsKruvpp7eLLZvDTC7bZuVtdAsZOapEVKCPORQX8EGTsjVkffGhBrwqrjdFCQuKBhIxiQp4fdTdw0PVkDjDph-yQpgaD_7w0e7OFek7qY0Ckmza1k_UKRySGntB7WbhB0GvYu00CWbhB0GvYnqNrlbAaJMJZ0kvaAWsXafQmza1k_UY01dI8IK6MnWhEwd4gNVXFEw69RzF7Ph4q823szQ9g8Cy13Wi8MdII6Mx_Y
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipes

2015-04-22 Thread Jeff Hewitt
Travis,

The question is does a mezzanine count as a story?  My past experience has 
been, NO, a mezzanine, that fits the definition of mezzanine in IBC, cannot 
also be a story, rather it is considered a part of the story within which it is 
contained.

Excerpts from IBC 2012









Jeff Hewitt, PE, SET, M.SFPE
Corporate Engineer


American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Wednesday, April 22, 2015 11:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Standpipes

No.  It is occupied.

There are all 1 story units on Level 1-3.  Level 4 has 1½ story units.
1000 sq ft on 4th floor, then go up a set of stairs that is internal to the 
unit.  The mezzanine/loft is about 400 sq ft.  It will have a bedroom and 
living space up there as well as a bathroom.

The architect has put confusing notes on the plan.  No one can figure it out.  
They are conflicting about NFPA 13 then 13R then standpipes, then no 
standpipes.  He has been asked to clarify, but it is taking longer than the 
builder wants.  They are just trying to get some ideas to know how it may go.

If this is a story that would drive standpipes, would it also not drive the 
building to an NFPA 13 system since it would then be 5 stories.  If the 
mezzanine/loft does not count as a story, then it would be applicable for 13R.  
They are under 2010 edition.  But, if the mezz/loft does not count as a story 
to drive it to 13, then does it count as an elevation to trigger standpipes?  
Lot's of questions.  Not many answers yet.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://cp.mcafee.com/d/k-Kr6xAg3zqb2pEV78CzBWXxKVJ6Wryqb2r29J6WryqbWqbVJ6Wryqb2r2pJ6WryqbwVdwS8A_ciDc5qHYpmS3IE-J6I_JeloixrBPuG_6lJwXafHhHfXjBm4EmVsSwXJxPbX_nV5BMszRXBQSm7-pKCMzORQX8FGT7csG7DR8OJMddECPhOrhWWl6O5bhAgYTsS02ltmg-AycendQmza1k_UKRySGn8lrxrW0E-l9QVSkvEJ6k2F_NU02rssKedwLQzh0cjS22QBLErhodPBLMtNtP
http://cp.mcafee.com/d/2DRPow720Qrhojd78V4QsLnsdTdETjsjhojohdETjsjhvjhvdETjsjhojojdETjsjhs79I6N4DVykVwHlvzaSMtB7RERDZFOH2kbsKrRnUOJI7phZqdp_qsGMB2TbCQ7tIepvvW_8IK3AuLsKCOM_PdQS4umKDp5dmUVzBgY-F6lK1FJcSqejqfniESgFqcy7CXCOsVHkiP2DeXrO5qBunNrifQMr5MIn3LF8z0K5gG9oqekQQnC4hPxEVjdQmza1k_UKRySGn8lrxrW0E-l9QVSkvEJ6k2F_NU02rssKedwLQzh0cjS22QBLErhodZFsr1iZZ
Send large files to us via: 
http://cp.mcafee.com/d/avndxMQ91NJ5xcQszAjhOZtMTsSztdNd5xdx4SztdNd5Zd5YSztdNd5xdxcSztdNd5MsCMr4ivC9jC2Jl-cHr1SkvmzmvSDaI9gJOVLlvzaSMtB7RERDZFOH2kbsKrgtSMVBZ_HYyOUehWZOWrb3_cTjohVqWtAkRrzCel3PWApmU6CSjpEVdEZtazp2BEO8urKr9PCJhbcasjAh9PSh_bUTwSbxoe-Ayc3t5EOwlf-bJoJGBO5mUm-wafBitetB7WbhB0GvYu00CT7bzzobZ8Qg34ZwwJ9rW6Qm3oOykULKkTaKJ

On 4/22/2015 9:17 AM, Matthew J Willis wrote:
 Sounds like an attic, not a loft.
 It will not be occupied right?


 R/
 Matt


 Matthew J. Willis
 Project Manager
 Rapid Fire Protection Inc.
 1805 Samco Road
 Rapid City, SD 57702
 Office-605.348.2342
 Cell-605.391.2733
 Fax:-605.348.0108



 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 David Autry
 Sent: Wednesday, April 22, 2015 10:09 AM
 To: 
 sprinklerforum@lists.firesprinkler.orgmailto:sprinklerforum@lists.firesprinkler.org
 Subject: RE: Standpipes

 Travis,
 I can't quote code. We had the same thing and the City required Standpipes.

 David Autry

 Meininger Fire Protection
 2521 West L Street, Suite 5
 Lincoln, NE 68522
 402.466.2616
 402.466.2617 fax
 da...@mfp-inc.commailto:da...@mfp-inc.com


 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 Travis Mack
 Sent: Wednesday, April 22, 2015 10:38 AM
 To: 
 sprinklerforum@lists.firesprinkler.orgmailto:sprinklerforum@lists.firesprinkler.org
 Subject: Standpipes

 Does a loft/mezzanine count toward the height to require a standpipe?

 Example: 4th floor is 29'-4 above lowest level of fire department access.
 So standpipe would not be required.

 But these units have a loft/mezzanine that will be obviously above the 30'. 
 The only way to access the loft is from a stair in the unit on the fourth 
 floor.

 So standpipes yes or no? It is an R-2 occupancy.

 Travis Mack, SET
 MFP Design, LLC
 Follow us on Facebook:
 http://cp.mcafee.com/d/k-Kr6wUedEI9CzAsyqenHK6XCQrFK9EI9I8CQrFK9ELFELC
 QrFK9EI9I9CQrFK9EK3AS3oyjYNasMlGLNBroeOzWQqP-QVlxa5KndWHYpmS3IE-J6I_Je
 loixrBPq3KS7cLLZvAmn1OfnKnjpovVCWr2fbnjIyCHssNOEuvkzaT0QSMrd79J7HFkr8k
 J6h3PtPpesRG9pxjDtJV2JiLbUJF7WodyUmbxTQAhwn2El4Id7aqqbP28VMQsFCWbhB0Gv
 YnqNrlbAaJMJZ0kvaAWsXafQmza1k_UY01dKen76MnWhEw69X11qiTQdEI6YuqA
 Send large files to MFP Design via:
 http

Re: A Poll of the Experienced

2014-12-05 Thread Jeff Hewitt
Mark, 

Which edition if IFC are you looking in?


Sent from my iPhone

 On Dec 5, 2014, at 9:09 PM, mphe...@aerofire.com mphe...@aerofire.com 
 wrote:
 
 Where are you guys finding these specific methods of proving the adequacy 
 of the fire flow requirements? I don't find any language close to this in the 
 IFC.  
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPhone
 
 On Dec 5, 2014, at 7:55 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 At 4 hydrants simultaneously if they're on the same water supply, or in 
 combination of public and private or at however many hydrants you have if 
 fewer than 4 and those being the sole source of fire flow.
 
 As other comments, I would reiterate that the Table B fire flow is for 
 outside hose streams only and completely separate and apart from any 
 hydraulic demand related to building sprinkler systems.
 
 Steve L.
 
 
 
 
 div Original message /divdivFrom: mphe...@aerofire.com 
 /divdivDate:12/05/2014  6:29 PM  (GMT-08:00) /divdivTo: 
 sprinklerforum@lists.firesprinkler.org /divdivSubject: Re: A Poll of the 
 Experienced /divdiv
 /divI think I agree with you, but to be very specific, let's assume I'm 
 designing a new building on a greenfield site which is served by a public 
 water system. The building is type V construction, 600,000 square feet and 
 fully protected with ESFR sprinklers. Table B105.2 indicated a fire flow 
 rate of 8000 GPM, reduced to 4000 GPM for sprinkler credit, at minimum 
 20psi. My question is, WHERE is this 4000 GPM at 20 psi measured? At the 
 city water main connection? Or at the fire pump discharge? 
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPhone
 
 On Dec 5, 2014, at 7:17 PM, Cahill, Christopher ccah...@burnsmcd.com 
 wrote:
 
 Neither.  It's the flow you need for a building. You might get it from a 
 muni or private. Absolutely nothing to do with sprinklers except you get a 
 reduction if building is sprinklered.
 
 
 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com
 
 
  Original message 
 From: mphe...@aerofire.com
 Date:12/05/2014 8:12 PM (GMT-06:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: A Poll of the Experienced
 
 Over this weekend I'd like to ask the opinion of those forumites 
 experienced in the reading and understanding of the International Fire  
 Code on the topic of Fire Flow described in Chapter 5, and further 
 prescribed in Appendix B. Is the available flow rate and residual pressure 
 referenced, intended to describe these values of the municipal or private 
 water supply available to the building site? Or, the minimum output of any 
 fire pump associated specifically with the automatic sprinkler system in 
 the building?
 Any takers? Questions? Clarifications?
 Thanks for any answers.
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPhone
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Seismic Design ASCE changing?

2014-09-15 Thread Jeff Hewitt
What is the occupancy of your job?



 On Sep 15, 2014, at 4:34 PM, Rod DiBona r...@rapidfireinc.com wrote:
 
 
 Just had an Engineer tell us that ASCE 7 is going to be changing so that 
 seismic design category B will require EQ for fire sprinkler systems and that 
 is why they are being proactive and requiring it now.  Thought I would run it 
 by the forum for the smell test. Thanks for any info. Thinking if Ken W 
 doesn't know about this that I might have to call BS..OR . I get 
 educated on current trends. Thanks.
 
 
 Rod at Rapid
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Water Supply Evaluation

2014-06-26 Thread Jeff Hewitt
Just wondering how an architect can be an EOR.  An architect is not an engineer.

Sent from my iPhone

 On Jun 26, 2014, at 10:25 AM, Tim Stone tston...@comcast.net wrote:
 
 Craig,
 
 In this case I was hired by the Architect to design a Sprinkler system for a
 brand new Church. The project is in a rural setting so fire pump and tanks
 are being used. Is it reasonable for the AHJ to expect the NICET certified
 designer to perform this duty or shouldn't this responsibility fall back
 onto the Architect who in this case would be the EOR?
 
 Regards,
 G. Tim Stone
 
 G. Tim Stone Consulting, LLC
 NICET Level III Engineering Technician
 Fire Protection Sprinkler Design
 and Consulting Services
 
 117 Old Stage Rd. - Essex Jct., VT. 05452
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
tston...@comcast.net
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of craig.pr...@ch2m.com
 Sent: Thursday, June 26, 2014 11:03 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Water Supply Evaluation
 
 Is your project a rural or suburban project?
 
 Fire flow requirements should be identified by the EOR with direction from
 the local or otherwise applicable fire authority.
 
 I typically make a call to the local fire authority to find out what method
 is used to determine fire flow.  There are several different methods out
 there with requirements that vary greatly so guessing isn't a wise move.
 
 Once we know their approved method, we apply that info and determine what is
 required to meet Code.  Sometimes that entails a tank and pump, sometimes
 not.  
 
 Fire Flow is one thing that gets overlooked a lot in engineering design.  We
 recently had one contractor telling an owner that the requirements for fire
 flow were ridiculous and he's never had to do that anywhere else.  I hope he
 doesn't do much design beyond 7-11 stores with his level of knowledge of the
 Codes.
 
 Craig L. Prahl 
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Steele, Andrew
 Sent: Thursday, June 26, 2014 10:47 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Water Supply Evaluation
 
 This most likely is from the International Fire Code, Chapter 5, Fire
 Service Features, (G) Section 507 Fire Protection Water Supplies.
 Subsection 507.3 says fire flow requirements for building or portions of
 building and facilities shall be determined by an approved method.
 In Ohio, this has been adopted direct into the Ohio Administrative Code.
 I'm guessing any other jurisdiction using ICC are (or will) be doing the
 same.
 
 Typically the local Fire Marshal will help facilitate the evaluation (to be
 conducted by a private fire protection/water utility contractor) and will be
 the one to review/approve it. 
 
 Andrew Steele
 Dayton, OH
 (937) 333-4522
 
 
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tim
 Stone
 Sent: Thursday, June 26, 2014 10:34 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Water Supply
 
 
 
 Has anyone in other parts of the country run across this?
 
 I just received a copy of a state fire marshal's review letter on a new
 project in which they are asking that the (Water supply for firefighting
 shall be evaluated and provided in accordance with NFPA 1142).
 
 
 
 Who is responsible for this evaluation in your area?
 
 
 
 Regards,
 
 G. Tim Stone
 
 
 
 G. Tim Stone Consulting, LLC
 
 NICET Level III Engineering Technician
 
 Fire Protection Sprinkler Design
 
 and Consulting Services
 
 
 
117 Old Stage Rd. - Essex Jct., VT. 05452
 
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
 
mailto:tston...@comcast.net
 tston...@comcast.net
 
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
 .org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___

RE: Minimum number of operating sprinklers

2013-08-07 Thread Jeff Hewitt
Reza,

Light hazard can be 225-sq.ft. per head not 130-sq.ft. for standard coverage, 
and up to 400-sq.ft per head if extended coverage could work.

If you were able to make extended coverage work, at say 400-sq.ft. per head, 
and took the quick response area reduction down to say 900-sq.ft. remote area, 
it is possible that you could fill out your 900-sq.ft remote area with just 3 
extended coverage heads (3 x 400-sq.ft. = 1200-sq.ft.), but NFPA 13 requires a 
minimum of 5 heads to be calculated.

Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reza 
Esmaeili
Sent: Wednesday, August 07, 2013 10:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Minimum number of operating sprinklers

According to NFPA-13, for designing a wet pipe sprinkler system in a light 
hazard occupancy, with a density of 0.1 gpm/ft2 operating over 1500 ft2 and 130 
ft2 per sprinkler, the number of operating sprinklers is calculated (1500/130) 
= 12. This is the minimum.

1- Can we use standard response sprinklers in a new building which is light 
hazard occupancy or we have to use quick response? If we have to use quick 
response sprinklers, so can we reduce area of operation by 40% and the new 
number would be 900 ft so the new number of operating sprinklers is (900/130)=7


2- NFPA-13 stating that The number of sprinklers in the design area shall 
never be less than five How this number is calculated? while the above 
calculations indicated that the minimum is either 12 or 7.

Thanks!
Reza
www.sarian.ir
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Minimum number of operating sprinklers

2013-08-07 Thread Jeff Hewitt
It is also possible that 4 standard coverage heads at 225-sq.ft could fill out 
a 900-sq.ft. remote area, but NFPA 13 requires a minimum of 5 heads.

Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, August 07, 2013 10:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Minimum number of operating sprinklers

Reza,

Light hazard can be 225-sq.ft. per head not 130-sq.ft. for standard coverage, 
and up to 400-sq.ft per head if extended coverage could work.

If you were able to make extended coverage work, at say 400-sq.ft. per head, 
and took the quick response area reduction down to say 900-sq.ft. remote area, 
it is possible that you could fill out your 900-sq.ft remote area with just 3 
extended coverage heads (3 x 400-sq.ft. = 1200-sq.ft.), but NFPA 13 requires a 
minimum of 5 heads to be calculated.

Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reza 
Esmaeili
Sent: Wednesday, August 07, 2013 10:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Minimum number of operating sprinklers

According to NFPA-13, for designing a wet pipe sprinkler system in a light 
hazard occupancy, with a density of 0.1 gpm/ft2 operating over 1500 ft2 and 130 
ft2 per sprinkler, the number of operating sprinklers is calculated (1500/130) 
= 12. This is the minimum.

1- Can we use standard response sprinklers in a new building which is light 
hazard occupancy or we have to use quick response? If we have to use quick 
response sprinklers, so can we reduce area of operation by 40% and the new 
number would be 900 ft so the new number of operating sprinklers is (900/130)=7


2- NFPA-13 stating that The number of sprinklers in the design area shall 
never be less than five How this number is calculated? while the above 
calculations indicated that the minimum is either 12 or 7.

Thanks!
Reza
www.sarian.ir
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Antifreeze

2013-08-05 Thread Jeff Hewitt
When specifically did you receive this NFSA EOD opinion?

Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Monday, August 05, 2013 8:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Antifreeze

Here is an informal interpretation on the issue:

Dear Mr. Wilson,

This email is in response to your request for an informal interpretation sent 
via...@nfsa.org.  You have referenced theTentative Interim Amendment (TIA) 
issued onthe 2011 Edition of NFPA 25 on March 1, 2011 (TIA 11-1).  
Specifically, you have asked if this is retroactive to older editions of NFPA 
25.

The answer to your question is “no.”  However, it is important to note that 
NFPA considers a new edition of a document to override the previous edition.  
In other words, when a new edition is published the old edition to no longer 
valid in the NFPA system.

When a standard is adopted into law with a specific edition, it may take time 
for that law to catch up with the new publications.  In these cases, it is 
important to understand the intent of the TIA and apply it as best as possible 
working with the jurisdiction.  When a TIA is issued by an NFPA Committee it is 
considered “emergency” information that the public needs to be aware of as soon 
as possible and therefore it cannot wait until the next revision of the 
document.

If you have any further questions, please do not hesitate to call me.

It should be noted that the above is my opinion.  It has not been processed as 
a formal interpretation in accordance with the NFPA Regulations Governing 
Committee Projects and should therefore not be considered, nor relied upon, as 
the official position of the NFPA or its Committees.

Very truly yours,

Victoria B. Valentine, P.E.

Director of Product Standards


Sent from my iPhone

On Aug 5, 2013, at 9:36 AM, Morey, Mike mo...@bmwc.com wrote:

 That's only for existing systems to remain in service as far as I know, from 
 the TIA:
 7.6.2.1
 Except as permitted in 7.6.2.2, antifreeze solutions shall be listed for use 
 in sprinkler systems. 
 7.6.2.2*
 Premixed antifreeze solutions of propylene glycol shall be permitted to be 
 used with ESFR sprinklers where the ESFR  sprinklers are listed for such use 
 in a specific application.
 
 
 
 Mike Morey, SET, CFPS
 Sprinkler Designer
 BMW Constructors, Inc.
 O: 317.651.0596 | C: 317.586.8111
 www.bmwc.com http://www.bmwc.com/
 
 
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of 
 accentf...@aol.com
 Sent: Mon 8/5/2013 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Antifreeze
 
 
 
 Gents:
 
 
 MY understanding of (current) requirements is - okay if pre-mixed in factory 
 (clearly marked on container) AND approved by licensed Fire Protection 
 Engineer...And YES, we continue to design using glycerin (CPVC) in 
 residential (including our previously cited $ 45M house here in NM)...
 
 
 
 Regards to all-
 
 
 
 Jerry
 
 
 accentf...@ao.com
 Santa Fe, New Mexico USA
 
 
 -Original Message-
 From: Morey, Mike mo...@bmwc.com
 To: sprinklerforum sprinklerforum@lists.firesprinkler.org
 Sent: Mon, Aug 5, 2013 7:23 am
 Subject: RE: Antifreeze
 
 
 Whether or not they enforce the bulletins, they are considered 
 retroactive to ALL editions.  Anyone installing a new AF system 
 without listed solution (which doesn't exist) puts themselves in great 
 legal peril from my understanding of the current situation.  Even the 
 premix on the market now no longer meets the requirements of the code.
 
 
 
 Mike Morey, SET, CFPS
 Sprinkler Designer
 BMW Constructors, Inc.
 O: 317.651.0596 | C: 317.586.8111
 www.bmwc.com http://www.bmwc.com/
 
 
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of 
 Forest Wilson
 Sent: Mon 8/5/2013 8:44 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Antifreeze
 
 
 
 It's worth noting that the bulletins issued by NFPA on antifreeze 
 affect the current edition of 13.
 Some states have previous versions of 13 adopted and don't enforce the 
 bulletins.
 
 
 
 Sent from my iPhone
 
 On Aug 5, 2013, at 7:43 AM, Craig Leadbetter craigleadbet...@gmail.com 
 wrote:
 
 I really appreciate the responses. I was looking for confirmation 
 that my thinking was correct. I lost a couple of bid jobs recently, 
 one which was a modification to an existing antifreeze system, 
 essentially tripling the size of the system, and the other was a wet and dry 
 system.
 
 I expected to lose the job that modified the antifreeze system. I 
 talked with the engineer prior to the bid but was told to bid what 
 was shown and it would be modified after

RE: Antifreeze

2013-08-05 Thread Jeff Hewitt
Check this link

http://nfpatoday.blog.nfpa.org/2012/08/new-anti-freeze-tias-approved-.html


Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Monday, August 05, 2013 8:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Antifreeze

Here is an informal interpretation on the issue:

Dear Mr. Wilson,

This email is in response to your request for an informal interpretation sent 
via...@nfsa.org.  You have referenced theTentative Interim Amendment (TIA) 
issued onthe 2011 Edition of NFPA 25 on March 1, 2011 (TIA 11-1).  
Specifically, you have asked if this is retroactive to older editions of NFPA 
25.

The answer to your question is “no.”  However, it is important to note that 
NFPA considers a new edition of a document to override the previous edition.  
In other words, when a new edition is published the old edition to no longer 
valid in the NFPA system.

When a standard is adopted into law with a specific edition, it may take time 
for that law to catch up with the new publications.  In these cases, it is 
important to understand the intent of the TIA and apply it as best as possible 
working with the jurisdiction.  When a TIA is issued by an NFPA Committee it is 
considered “emergency” information that the public needs to be aware of as soon 
as possible and therefore it cannot wait until the next revision of the 
document.

If you have any further questions, please do not hesitate to call me.

It should be noted that the above is my opinion.  It has not been processed as 
a formal interpretation in accordance with the NFPA Regulations Governing 
Committee Projects and should therefore not be considered, nor relied upon, as 
the official position of the NFPA or its Committees.

Very truly yours,

Victoria B. Valentine, P.E.

Director of Product Standards


Sent from my iPhone

On Aug 5, 2013, at 9:36 AM, Morey, Mike mo...@bmwc.com wrote:

 That's only for existing systems to remain in service as far as I know, from 
 the TIA:
 7.6.2.1
 Except as permitted in 7.6.2.2, antifreeze solutions shall be listed for use 
 in sprinkler systems. 
 7.6.2.2*
 Premixed antifreeze solutions of propylene glycol shall be permitted to be 
 used with ESFR sprinklers where the ESFR  sprinklers are listed for such use 
 in a specific application.
 
 
 
 Mike Morey, SET, CFPS
 Sprinkler Designer
 BMW Constructors, Inc.
 O: 317.651.0596 | C: 317.586.8111
 www.bmwc.com http://www.bmwc.com/
 
 
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of 
 accentf...@aol.com
 Sent: Mon 8/5/2013 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Antifreeze
 
 
 
 Gents:
 
 
 MY understanding of (current) requirements is - okay if pre-mixed in factory 
 (clearly marked on container) AND approved by licensed Fire Protection 
 Engineer...And YES, we continue to design using glycerin (CPVC) in 
 residential (including our previously cited $ 45M house here in NM)...
 
 
 
 Regards to all-
 
 
 
 Jerry
 
 
 accentf...@ao.com
 Santa Fe, New Mexico USA
 
 
 -Original Message-
 From: Morey, Mike mo...@bmwc.com
 To: sprinklerforum sprinklerforum@lists.firesprinkler.org
 Sent: Mon, Aug 5, 2013 7:23 am
 Subject: RE: Antifreeze
 
 
 Whether or not they enforce the bulletins, they are considered 
 retroactive to ALL editions.  Anyone installing a new AF system 
 without listed solution (which doesn't exist) puts themselves in great 
 legal peril from my understanding of the current situation.  Even the 
 premix on the market now no longer meets the requirements of the code.
 
 
 
 Mike Morey, SET, CFPS
 Sprinkler Designer
 BMW Constructors, Inc.
 O: 317.651.0596 | C: 317.586.8111
 www.bmwc.com http://www.bmwc.com/
 
 
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of 
 Forest Wilson
 Sent: Mon 8/5/2013 8:44 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Antifreeze
 
 
 
 It's worth noting that the bulletins issued by NFPA on antifreeze 
 affect the current edition of 13.
 Some states have previous versions of 13 adopted and don't enforce the 
 bulletins.
 
 
 
 Sent from my iPhone
 
 On Aug 5, 2013, at 7:43 AM, Craig Leadbetter craigleadbet...@gmail.com 
 wrote:
 
 I really appreciate the responses. I was looking for confirmation 
 that my thinking was correct. I lost a couple of bid jobs recently, 
 one which was a modification to an existing antifreeze system, 
 essentially tripling the size of the system, and the other was a wet and dry 
 system.
 
 I expected to lose the job that modified the antifreeze system. I 
 talked with the engineer prior to the bid but was told to bid what

RE: Home Fire Sprinkler Guidance - New Jersey

2013-07-30 Thread Jeff Hewitt
Why install sprinklers according to NFPA 13 then?  It's just a standard, a 
regulation.  Why not just do what you want?

Jeff Hewitt, PE, SET
Corporate Engineer
   
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop
Birmingham, AL  35210
205-591-9111 ext. 1452
205-591-9990 (Fax)
205-317-0918 (cell)

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Tuesday, July 30, 2013 10:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Home Fire Sprinkler Guidance - New Jersey

Im a marathon runner. 
I drink raw vegetable juice, eat mostly plant diet and meat on occasion. 
The entire country is dying from obesity and obesity related illnesses. 
Many more than die in fires. 

Now the people have decided to mandate health insurance coverage. Those who 
do not comply are subject to arrest. 

The people of NYC are now regulating various portion sizes in restaurants so 
fat people won't eat more. 

Do I have the moral right to tell another person what food to eat or what 
exercise to do?
I don't think so. 
Do I have the moral right to tell them how many kids to have? (the people of 
china have already done this). 

If I don't exercise, drink booze and smoke cigarettes I will become Ill. My 
illness will affect society to a limited degree.  In fact billions are spent on 
healthcare. 

I don't need the people to tell me how to eat food or how to exercise. Jack 
Lelane didn't need the people or government to tell him how to be healthy. 

In my city they have a new lawn policeman that drives around writing tickets 
for uncut lawns. As with any other government regulation if you don't comply 
you are subject to arrest and imprisonment. Hes probably making a good wage and 
government union benefits as Ohio has lost most major employers and cities are 
broke. 

I'm curious how many will support government mandates if all citizens were 
ordered to cut all fat food, destroy all booze and cigarettes and run a 
marathon in a year or be imprisoned. 

It's a different issue? It's just a building code, it's just a healthcare law, 
it's just an anti trust law, it's just a no smoking law, it's just a minor 
regulation. 

For 100 years people installed sprinklers in buildings without the government 
mandating it. 

I stay very healthy, somehow without mandates from the people. 
Eventually there will be nothing left to mandate or regulate. 


Sent from my iPhone

On Jul 30, 2013, at 11:22 AM, Ron Greenman rongreen...@gmail.com wrote:

 Ben won't go to jail because he didn't put in sprinklers but he'll be 
 denied a certificate of occupancy and when he feels tha Virginia City 
 is creeping too close to the Ponderosa and the good people of that 
 burg are creating too many laws that infringe on his personal rights 
 to ignore the rules of society while still reaping its benefits and he 
 wants to move he won't be able to sell the Ponderosa because he built a 
 substandard house.
 Of course if Sheriff Coffee is doing his job a Do Not Occupy notice 
 will have been posted, no utilities will have been allowed to connect, 
 and if Ben decided to squat he would be subject to arrest for not 
 complying with the Do Not Occupy order, not because he didn't install 
 sprinklers, a law the society agreed was for the good of all.
 
 I remember a Mad Magazine parody of Bonanza from when I was a kid. Two 
 things stand out fifty plus years later: 1. Hoss was called Ox, and 2.
 After an exhausting multi-day ride from the train station to the 
 house, the reporter that was visiting the Ponderosa was asked if he 
 was hungry. Upon answering affirmatively Ben stated, Well, we better 
 get started. It's a three day ride to the kitchen. Most of us though 
 live in the city or suburbs, packed close together. Set-backs are 
 agreements between us as to how, among other things, to not expose 
 each others' risky behaviors. We each have to maintain five feet of 
 clearance from our mutual property line because we've decided that ten 
 feet of separation is a good idea. Now does this onerous law not apply 
 to you? Doesn't it infringe on your right to use your land as you 
 wish? Doesn't your liberty then force me to build my house ten feet 
 from the line, infringing on my right to use my land as I wish, if I 
 want to maintain a safe distance from your selfishness. Or perhaps 
 I'll use my land in our suburban neighborhood for all day/every day 
 open air rap concerts, or for my steel mill. I ought not have to deal 
 with zoning laws that infringe on my freedoms. Remember that most 
 houses change hands every five years. Building codes assure me that if 
 I'm buying your house it was built to a standard acceptable to all at 
 the time of construction. Remember that I can't see if you built your 
 walls with studs randomly spaced of near three foot enters, wired it 
 with lamp cord, and used Cheerios for insulation

RE: Bedbugs

2013-02-28 Thread Jeff Hewitt, PE
Check NFPA 13, 2013, 6.2.1.1 


Jeff Hewitt, PE, SET  |  Corporate Engineer 
NICET #102015  |  Water Based Layout - Level IV
Inspection Testing  Maintenance - Level III

241 Hughes Lane  |  St. Charles, MO 63301
Office 636-946-0011  |  Fax 636-946-5172
Cell 314-574-6989  |  www.bistatefire.com

Fire sprinklers save lives.  Can you live without them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John O'Connor
Sent: Thursday, February 28, 2013 1:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Bedbugs

Gentlemen:

Paragraph 6.2.1 (2007 Ed. NFPA-13) states:  Only new sprinklers shall be
installed.
This refers to new work.  We relocate sprinklers in office environments all
the time.  Where does it say specifically that if you unscrew and remove a
head, you replace it?  What about general maintenance such as internal
inspections, where one head is to be removed for a visual inspection inside
the fitting?  You infer that the only correct action is replacing every head
you ever remove.  I say you are reading more into the code than intended.
If they wanted only new heads for every action, they (the committee) would
have said so. 

Reference also the 2002 edition of the Automatic Sprinkler Handbook, page
106, para 6.1.2.2 where they discuss reconditioned components.  However,
when sprinklers have been installed in a building on a temporary basis--for
example, prior to finish ceiling work--the same sprinklers can be used on
that job.  The same holds true for an existing system that is being lowered
to accommodate a new ceiling provided the sprinklers are of the proper
orientation and the associated hazard has not changed.

The committee has clearly allowed relocated heads to be used.  If the
occupancy has not changed, the original head, as in the case of the bed-bug
remediation example, can be reused.  Obvious exceptions are if the head(s)
are 50 years or older, or of the wrong orifice, temp, thread size etc,
precluding its applicability as a suitable head for reinstallation.

John O'Connor 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Denhardt
Sent: Thursday, February 28, 2013 12:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Bedbugs

Absolutely


John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd - Work
Sent: Thursday, February 28, 2013 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Bedbugs

Aren't you supposed to replace with new heads if the old ones are unscrewed?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1430 / Virus Database: 2641/5638 - Release Date: 02/28/13

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: 18 Clearance

2012-11-29 Thread Jeff Hewitt, PE
The 18-in. clearance is required when trying to throw water over an
obstruction to maintain coverage on the other side.

In your case, with a branch line down each aisle, it seems to me that you
are NOT throwing water over an obstruction, and are more similar to the
rules for storage along walls, as outlined in NFPA 13, 2010, A.8.6.6

the 18-in. dimension is not intended to limit the height of shelving on a
wall or shelving against a wall in accordance with 8.6.6, 8.7.6, 8.8.6, and
8.9.  Where shelving is installed on a wall and is not directly below
sprinklers, the shelves, including storage thereon, can extend above the
level of a plane located 18-in. below ceiling sprinkler deflectors.

Commentary to 8.6.6.1 states

sprinklers installed near wall mounted shelves or piled storage located
against a wall are not intended to be governed by the requirements of
8.6.6.1.  The clear space beneath a sprinkler is needed for the spray
pattern to fully develop to allow proper wetting of the floor and not the
wall.



Jeff Hewitt, PE, SET  |  Corporate Engineer 
NICET #102015  |  Water Based Layout - Level IV
Inspection Testing  Maintenance - Level III

241 Hughes Lane  |  St. Charles, MO 63301
Office 636-946-0011  |  Fax 636-946-5172
Cell 314-574-6989  |  www.bistatefire.com

Fire sprinklers save lives.  Can you live without them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Gregory
Lindholm
Sent: Thursday, November 29, 2012 9:56 AM
To: SprinklerFORUM
Subject: 18 Clearance



We have an AHJ that told a customer that they have to keep the storage on
shelves at least 18 below the level of the sprinkler heads.
 
It is an auto parts store where they have the typical walkways between rows
of bins/shelves of auto parts, etc. It is only about 7 1/2 feet to the deck,
and there is a branch line down each aisle.
 
I know that it is allowable to be above the 18 level in closets, etc., but
would that apply in instances like this? (I see this setup quite
frequently.)

Greg Lindholm
 

  
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121129/e3de1c4d/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Good one for a Friday

2011-12-09 Thread Jeff Hewitt, PE
Should a NICET technician be determining this design criteria?  








Jeff Hewitt, PE, SET  |  Corporate Engineer 
NICET #102015  |  Water Based Layout - Level IV
Inspection Testing  Maintenance - Level III

241 Hughes Lane  |  St. Charles, MO 63301
Office 636-946-0011  |  Fax 636-946-5172
Cell 314-574-6989  |  www.bistatefire.com

Fire sprinklers save lives.  Can you live without them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim Davidson
Sent: Friday, December 09, 2011 10:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Good one for a Friday

Robert,

Before we can answer you need to find out type of crude, some crude oil can
be considered extremely toxic because of trapped gases within the crude,
other crude can be extremely light with light hydrocarbon components,
someone (EOR of owner) needs to tell you what the products is and I would
start with Foam or AFFF systems not water. 

Before you start design have the owner's EOR get the details to you so you
can make an informed decision on the design of the system. Also reminder to
document what you find and how you developed you design criteria and have
the owner and his EOR sign off on it.

Have a fire safe Holiday season!!

Regards

Jim  

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Robert
Thompson
Sent: Friday, December 09, 2011 10:15 AM
To: sprinklerforum@firesprinkler.org
Subject: Good one for a Friday

Indoor rail car loading of crude oil.  design dry system water only .3/6000
sqft at deck and under obstructions.  100 sqft spacing of 11.2k sprinklers.
Right track or way off.   Don't see everyday but may in future.

Thank You
Robert Thompson
Certified Engineering Technologist

Dakota Fire Protection
1710 North Washington Street
Grand Forks, ND 58203
Phone: 701-772-8820
Fax: 701-772-7932
Email: rob...@dakotafire.com




-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111209/a526975d/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Table 17.3.3.1 ESFR Protection

2011-09-12 Thread Jeff Hewitt, PE
Randy,

There is no error.  Not all ESFR are created equal.  K25 and K22 will not
protect the same things that K14 and K17 will.


Jeff Hewitt, PE, SET
Corporate Engineer

   BI-STATE 
  FIRE PROTECTION
C  O  R  P  O  R  A  T  I  O  N
   

 636-946-0011  office
 636-946-5172  fax
 314-574-6989  cell

Fire Sprinklers save lives.  Can you live without them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Randy Knutson
Sent: Monday, September 12, 2011 3:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Table 17.3.3.1 ESFR Protection 

Is there an error in Table 17.3.3.1?

I notice in exposed unexpanded 35ft storage in 40ft building section there
is a big penalty for using 25.2k sprinklers.

14.0k at 75psi ~ 121gpm

16.8k at 52psi ~ 121gpm

25.2k at 50psi ~ 178gpm

 

For the same heights with cartoned unexpanded, the numbers are the same with
the exception of 25psi for the 25.2k.

 

I checked the errata for NFPA 13 2010ed and didn't see anything. 

 

Randy Knutson, CET

Sales Manager

Shilo Automatic Sprinkler, Inc.

(208) 412-6113 cell

(208) 466-0006 ext 119

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20110912/fcff7a3d/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: staggered ESFR sprinklers

2011-08-30 Thread Jeff Hewitt, PE
Roland, 

Thank you for the correction.  I forgot about that change in 2010 edition,
which is actually not referenced yet by any building code, so depending on
the jurisdiction, we may not be able to use that.




Jeff Hewitt, PE, SET
Corporate Engineer

   BI-STATE 
  FIRE PROTECTION
C  O  R  P  O  R  A  T  I  O  N
   

 636-946-0011  office
 636-946-5172  fax
 314-574-6989  cell

Fire Sprinklers save lives.  Can you live without them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, August 30, 2011 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: staggered ESFR sprinklers

There is no longer a 960 sf minimum size

Roland

On Aug 30, 2011, at 7:37 AM, Jeff Hewitt, PE wrote:

 If this design does move forward, another concern would be your  
 design area.
 Sounds like you may need more than 12 heads to fill up your minimum  
 960
 sq.ft.




 Jeff Hewitt, PE, SET

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Commodity classification of Lard

2011-07-19 Thread Jeff Hewitt
Looking at the MSDS, it has a Flash Point of 419-deg. F (215 deg C), and
could be considered a combustible liquid subject to NFPA 30, even though it
is stored in solid form. I would also look at butter or margarine as
possible comparables, and also vegetable oil.

My opinion is that this would be classified as a Class IIIB Liquid in NFPA
30.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard
Lindner
Sent: Tuesday, July 19, 2011 3:58 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Commodity classification of Lard

And for those that might not completely understand (like me), how do we take
this type of MSDS info and extropolate it into a design? Can you give me a
gentle poke in the right direction.

Richard

On Tue, Jul 19, 2011 at 3:40 PM, Thom tmcma...@firetechinc.com wrote:

 http://www.sciencelab.com/msds.php?msdsId=9924458


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
 Martinez
 Sent: Tuesday, July 19, 2011 1:12 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Commodity classification of Lard

 Anyone know what the commodity classification of animal fat lard would
 be?  I didn't see anything in NFPA or FM on this after a quick review.
 I have a refrigerated storage area with wood pallets containing 64 - 50
 lbs blocks of lard in which each block is placed in a plastic bag and
 enclosed in corrugated cardboard box.
 Thanks,


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Commodity classification of Lard

2011-07-19 Thread Jeff Hewitt
Lard oil, bottled/cartoned, or lard, packaged/cartoned, will still be a
Class IIIB Liquid

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, July 19, 2011 4:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Commodity classification of Lard

The MSDS cited is for Lard Oil, which may behave differently than solid
blocks of Lard. Need to fully research. Refer back to my comment about it
being the PE's job to evaluate.

Now if you bought I Can't Believe It's Not Lard..


At 05:12 PM 7/19/2011, you wrote:
Looking at the MSDS, it has a Flash Point of 419-deg. F (215 deg C), and
could be considered a combustible liquid subject to NFPA 30, even though it
is stored in solid form. I would also look at butter or margarine as
possible comparables, and also vegetable oil.

My opinion is that this would be classified as a Class IIIB Liquid in NFPA
30.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard
Lindner
Sent: Tuesday, July 19, 2011 3:58 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Commodity classification of Lard

And for those that might not completely understand (like me), how do we
take
this type of MSDS info and extropolate it into a design? Can you give me a
gentle poke in the right direction.

Richard

On Tue, Jul 19, 2011 at 3:40 PM, Thom tmcma...@firetechinc.com wrote:

 http://www.sciencelab.com/msds.php?msdsId=9924458


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
 Martinez
 Sent: Tuesday, July 19, 2011 1:12 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Commodity classification of Lard

 Anyone know what the commodity classification of animal fat lard would
 be?  I didn't see anything in NFPA or FM on this after a quick review.
 I have a refrigerated storage area with wood pallets containing 64 - 50
 lbs blocks of lard in which each block is placed in a plastic bag and
 enclosed in corrugated cardboard box.
 Thanks,


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Sleeves

2011-07-07 Thread Jeff Hewitt
Bobby,

I would suggest that the use of a sleeve depends on the UL Through
Penetration System you choose to use for the penetration.  Some do not
require the use of sleeves.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, July 07, 2011 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe Sleeves

We have an existing school we are sprinkling. When we pass through a block
wall, non-rated (smoke, fire etc.) we plan on providing clearance or a flex
coupling within a foot of the wall on both sides of the wall. Does it say
anywhere we have to use sleeves for block walls? We will be using Sch. 10 
40 pipe as well as CPVC. I can't seem to find anything other than NFPA 13 -
2007 9.3.4.3 Where clearance is provided by a pipe sleeve.. But nothing
requiring one.

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: recommended pre-action system

2011-05-11 Thread Jeff Hewitt
Joel,

If you can convince them that the likelihood of accidental discharge is
extremely low, then I would suggest a much cheaper alternative for this
small space, protect the space as ordinary hazard instead of light hazard,
space the heads accordingly, and because it is now OH, it does not have to
be QR, so install SR, fusible link, IM or high temperature heads.  

This should alleviate any other water damage concerns, as the head response
should now be sufficiently slow that if there is a fire and these heads do
open, the equipment is beyond repair anyway due to smoke/heat damage that
occurred prior to sprinkler activation.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joel Chaim
Sent: Wednesday, May 11, 2011 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: recommended pre-action system

I have a job that requires 3 sprinkler head in a server room and the
customer wants us to install a pre-action system. what model is the simplest
to use?

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: recommended pre-action system

2011-05-11 Thread Jeff Hewitt
I agree George,

I left that part out in my previous post do it as a simple wet system, with
SR, IM or High temp. fusible link heads

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Wednesday, May 11, 2011 2:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: recommended pre-action system

We prefer to do these as simply as possible-
Concealed sprinklers to aid in protection from mechanical injury, wet.

And Since Viking and Victaulic have chimed in, we should expect other mfrs
that also offer a prepack to chime in, or at least now know that there are
multiple choices if you need to go prepack due to installation competency
concerns.

Speaking of which, a well-installed simple wet system would be my preference
over a prepack installed incompetentlyno matter how simple they've tried
to make it.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, May 11, 2011 3:03 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: recommended pre-action system

Joel,

If you can convince them that the likelihood of accidental discharge is
extremely low, then I would suggest a much cheaper alternative for this
small space, protect the space as ordinary hazard instead of light hazard,
space the heads accordingly, and because it is now OH, it does not have to
be QR, so install SR, fusible link, IM or high temperature heads.  

This should alleviate any other water damage concerns, as the head response
should now be sufficiently slow that if there is a fire and these heads do
open, the equipment is beyond repair anyway due to smoke/heat damage that
occurred prior to sprinkler activation.

Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State
Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joel Chaim
Sent: Wednesday, May 11, 2011 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: recommended pre-action system

I have a job that requires 3 sprinkler head in a server room and the
customer wants us to install a pre-action system. what model is the simplest
to use?

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Electronic Submissions

2011-04-15 Thread Jeff Hewitt
As a licensed PE that stamps a lot of documents, I have a few thoughts for
you.

I had some good advice given back when I first obtained my license.  I keep
a written log of EVERYTHING that I stamp, so that I have an established,
consistent, living document to prove whether I actually signed something or
not.  In addition, I sign in different colors of ink.  I may use blue, black
or red, ball point or gel, and always sign my log book with the same pen
that I sign the documents with.

As for putting your stamp on a document, I believe that you must put your
stamp on it, regardless, but not necessarily sign it.  Most states will take
the position that your stamp must be present to identify who is responsible
whether signed or not.  You sign it when it is for a permit or some other
official/legal purpose.

I am not concerned about theft or misuse of my stamp.  I have myself
reasonably protected with my log, and would welcome suing the pants off
anyone that I caught using my stamp/identity.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Friday, April 15, 2011 10:57 AM
To: sprinklerforum@firesprinkler.org; 'Coastal'
Subject: RE: Electronic Submissions

No matter what you do or what security procedures you follow, someone
somewhere will find and use some method to get around that protection. So do
the best you can reasonably do to protect your seal or signature, and as
others have said, your submitting to the AHJ, not the general public. That
alone provides a certain level of security. If the Arch. Or GC requires
copies of approved drawings, there really isn't much you can do to keep them
from photocopying the seal or signature, and using it elsewhere. We have
always had a policy that all signatures must be in colored ink, so we could
spot photocopies. Did it help? Were there still ways around it? You bet!
Do your best, and hope that it never becomes an issue. If it does become an
issue, find a really good lawyer and sue the crap out of the offender!

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Friday, April 15, 2011 7:41 AM
To: sprinklerforum@firesprinkler.org; Coastal
Subject: Re: Electronic Submissions

I have seen several situations where contractors have scammed PE stamps for
drawings (including sticky back stamps from previous drawings and one
company actually using a dead PE's stamp). This has made me get a little
paranoid about the whole thing. In MA, the stamp not only has to be signed,
but dated (I typically do this for all stamps). Doing this electronically
would add a level of complexity, but help prevent lifting. There are also
some AHJs around here that require wet stamps on all drawings and will not
accept copies. 


At 07:25 AM 4/15/2011, you wrote:
Hello,

It is an option to submit for state review and approval in South Carolina.
I have used it a couple of times. Works ok for me.


As far as somebody removing your stamp from a drawing.

Insert stamp on finished drawing.

Print to PDF

No security needed as there is noting to select and grab. It was printed
into the set.

Friday, April 15, 2011, 6:48:31 AM, you wrote:

 Aren't we only submitting stamped and signed documents to AHJ's?  I think
 that would help limit security issues.  When I worked for an engineer,
they
 only stamped and signed documents submitted for permit and were pretty
 adamant about it.  Of course, that was before cad really became the norm
and
 we were using sticky-back for standard details.
 I've become accustomed to Bluebeam and really like it for coordination,
some
 submission work so far, and just not having so much paper to deal with.
I
 look forward to working this way much more.
 I just wish I could crack that adobe requirement with NFPA standards.
 TD


 The digital stamp itself cannot be copied out of the file, it can't even
be
 selected at times, and you have the option of viewing the original.
There
 are some pretty in depth security measures available (no printing, no
 deletion of individual sheets, no commenting, password protection,).  It
 could become a screen shot then transferred but that would be no
different
 than scanning a physical print.  I haven't gotten into it fully, but have
 gotten a couple PDF's that had these measures in place.

 http://www.adobe.com/security/pdfs/acrobat_livecycle_security_wp.pdf
 In your free time

 Locks are for honest people...as I was once told. 


 Sounds like it could be easy for the unscrupulous contractor to lift a
 stamp. What is there for security?

 Sent from my iPhone

RE: In-rack sprinkler maximum and minimum spacing...

2011-03-29 Thread Jeff Hewitt
Try NFPA 13, 2002, Table 12.3.2.4.2.1

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sean Lockyer
Sent: Tuesday, March 29, 2011 2:14 PM
To: sprinklerforum@firesprinkler.org
Subject: In-rack sprinkler maximum and minimum spacing...

I have a fire marshal wanting me to show him where in NFPA 13 it dictates
the minimum and maximum spacing of in-rack sprinklers. This is a good
question, for the life of me I have never found it in black and white. I
know that there are several references to 8'-0 maximum spacing per
sprinkler for storage up to 25'-0 but we are only storing up to 20'-0.

I have always been under the impression that you space a sprinkler in each
in-rack flue space, usually on the center point of the rack or at the rack
upright. Normally the racks are spaced around 8'-0 O.C. but there is one
here that is 4'-0 O.C. We are using intermediate level in-rack sprinklers
with the overhead system being ELO sprinklers-no ESFR, Large Drop, etc...

We are using NFPA 13, 2002 Edition here in Florida. What says the community
?

-- 
Sean Lockyer
Project Designer
Delta Fire Sprinklers
(407) 328-3000, ext 139
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: partial walls in mech rooms

2011-03-10 Thread Jeff Hewitt
NFPA 13, 2010, 8.15.22.3 only applies when open to an adjacent space on ONE
side only.  Maybe I am wrong, but based on what has been described sounds
like it is open on ALL sides, thus 8.15.22.3 does not apply.  This described
situation would require sprinklers at the deck over the entire area because
a concealed space has not been created (due to the described space being
open on all sides).

Providing sprinklers at the deck for 24-ft. beyond, on all sides is not
correct.

Just my opinion.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Thursday, March 10, 2011 10:45 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: partial walls in mech rooms

Well, you have to go 24 feet which ends up being an area of approx, 55' x
54' that you are now required to put heads in. I Although the example in the
handbook refers to a warehouse/office space in which the clarification is
that protection must extend 24' over the offices and the area of greater
hazard is outside the 24' zone, I guess it is similar, but it is a stretch
in my opinion.

In this case, the greater hazard is surrounded by a lesser hazard on 4
sides, Therefore if 8.15.22.3 applies, we will end up protecting the entire
non-combustible interstitial space. Before I argue for this change order I
want to make sure this is the intent on the code.

Thanks,
Greg

On Thu, Mar 10, 2011 at 10:31 AM, Bob Knight bkni...@agfsi.com wrote:

 I think in this case you are cooling the structure in an area that heat
 could become a factor.  2010 ed. Requires .6 times the sq rt of the area
or
 a minimum of 24' extended into areas such as this (8.15.22.3  .4).

 BK

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:
 sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline
 Sent: Thursday, March 10, 2011 9:10 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: partial walls in mech rooms

 I cannot get past the idea that we normally put water on floors, not on
the
 tops of ceilings!

 -Original Message-
 From: Greg McGahan [mailto:g...@livingwaterfp.com]
 Sent: Thursday, March 10, 2011 10:00 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: partial walls in mech rooms

 It is not CLEAR, this section appears to refer to the cloud situation we
 are often running into.

 I am not trying to get out of something here, I am trying to document why
 we have to do it. We have used the 15' rule in the past, but again, that
is
 truly intended for another situation, in my honest opinion. This section
is
 to avoid fusing heads in adjacent areas, not require additional
 protection... as I read it.

 On Thu, Mar 10, 2011 at 9:47 AM, Morey, Mike mo...@bmwc.com wrote:

  On second reading, if you're saying the LH areas have a ceiling but
  the mechanical rooms don't then 8.15.22 does apply, in which case the
  higher area is the roof deck, which means you provide the protection
  for the mechanical room at the deck and for 24' in any direction away
  from the mechanical room over the ceiling of the LH space.
 
  -Mike Morey, SET
  Sprinkler Designer
  BMW Constructors, Inc.
  office: 317-651-0596
  mobile: 317-439-2695
 
  
 
  From: sprinklerforum-boun...@firesprinkler.org on behalf of Greg
  McGahan
  Sent: Thu 3/10/2011 10:21 AM
  To: sprinklerforum@firesprinkler.org
  Subject: partial walls in mech rooms
 
 
 
  We have an issue right now with a light hazard non-combustible
  building in which there are multiple small mechanical rooms -3' x 8'
  or 6' x 7' in general size. The architect was vague so the GC is not
  putting in ceilings nor is he running the walls up to the deck.
 
  I have been reading and rereading chapter 8 of 13 -2010 edition, and I
  cannot conclusively determine what we are required to do in this case.
  The description in 8.15.22.1 is not exactly correct so I can't see
 clearly...
 
  Does anybody have a cut and dry answer?
  Thanks,
  Greg
 
  --
  Greg McGahan
  Living Water Fire Protection, LLC
  1160 McKenzie Road
  Cantonment, FL 32533
  850-937-1850
  fax 850-937-1852
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  For Technical Assistance, send an email to: supp...@firesprinkler.org
 
  To Unsubscribe, send an email
  to:sprinklerforum-requ...@firesprinkler.org
  (Put the word unsubscribe in the subject field)
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org

RE: sprinkler escutcheons and rated ceilings

2011-02-22 Thread Jeff Hewitt
Try IBC, 2009 713.3.2 Exception 5

And associated Figure 713.3.2(2)



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Don Lowry
Sent: Tuesday, February 22, 2011 1:52 PM
To: sprinklerforum@firesprinkler.org
Subject: sprinkler escutcheons and rated ceilings

Forumites,

We have one of those overzealous inspectors from “Dept of Aging and
Disability Services” (DADS) TX who all of a sudden decides that the holes in
the UL Listed recessed (RASCO FP) escutcheon  somehow nullifies the rated
ceiling construction in Nursing Homes.  Even with the listing bulletins.  I
understand that the holes are how the sprinkler got its rating, but anyone
have a quick document that’s states the obvious?

Thanks in Advance

Don Lowry, RME
Dickerson Fire Protection

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Canopy projecting from wall

2011-02-18 Thread Jeff Hewitt
Dewayne,

4-ft wide and 18-in. down is correct if the obstruction is in the middle of
the space where water can throw over the top of the obstruction.  However,
you also said the canopies protrude from the wall, so now the 4-ft wide
exemption does not apply.  Water cannot throw on both sides of the canopy
if it is against the wall.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Friday, February 18, 2011 3:56 PM
To: sprinklerforum@firesprinkler.org
Subject: Canopy projecting from wall

I have a situation where I have a room with 18ft acoustical ceilings and
a couple of non-combustible canopies projecting from a wall around 9ft
AFF.
The canopies themselves protrude from the wall only 3ft and are about
8ft long each.  I don't think I would need additional protection below
the canopies since the overhead ceiling is fully sprinkled, the canopies
are less than 4ft wide and at least 18 down from the overhead
sprinklers, and no additional floor area is created.
What does the forum think?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: @#*% Hose Stations

2010-12-20 Thread Jeff Hewitt
If this is not a design-build project, and the specs do not require them,
even though the AHJ does, then I agree, the plumber that wrote the FP specs
blew it.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Monday, December 20, 2010 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: @#*% Hose Stations

I know this is a no brainer but any help would be appreciated. We are doing
a warehouse system with ESFR heads, shop drawings were approved by all
parties, Architect, Engineer, AHJ. The only comment was from the AHJ that
stated he wanted (3) hose stations added, no big deal. We send the GC a
change order for the addition of the hose stations and it gets approved; now
the GC wants us to provide additional information as to why we didn't
include hose station in our original bid. We explained that there were no
hose stations shown in the contract drawings or in the spec's and that
NFPA-13 doesn't require them. Apparently the owner is trying to get the GC
to pay for them because he didn't consult his crystal ball when he bid it
and should have seen that the AHJ was going to add them! I know we're clean
from our end but was just trying to help the GC out, any ideas?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16540)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: @#*% Hose Stations

2010-12-20 Thread Jeff Hewitt
OK, I stand corrected.  The plumber that prepared the FP specs did not know
which boxes to click from their master spec writing software.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: Jeff Hewitt [mailto:je...@bistatefire.com] 
Sent: Monday, December 20, 2010 3:24 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: @#*% Hose Stations

If this is not a design-build project, and the specs do not require them,
even though the AHJ does, then I agree, the plumber that wrote the FP specs
blew it.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Monday, December 20, 2010 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: @#*% Hose Stations

I know this is a no brainer but any help would be appreciated. We are doing
a warehouse system with ESFR heads, shop drawings were approved by all
parties, Architect, Engineer, AHJ. The only comment was from the AHJ that
stated he wanted (3) hose stations added, no big deal. We send the GC a
change order for the addition of the hose stations and it gets approved; now
the GC wants us to provide additional information as to why we didn't
include hose station in our original bid. We explained that there were no
hose stations shown in the contract drawings or in the spec's and that
NFPA-13 doesn't require them. Apparently the owner is trying to get the GC
to pay for them because he didn't consult his crystal ball when he bid it
and should have seen that the AHJ was going to add them! I know we're clean
from our end but was just trying to help the GC out, any ideas?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16540)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: FPE

2010-12-15 Thread Jeff Hewitt
Garth,

I would say for a legit FPE (Fire Protection Engineer), the answer should be
YES.  However, most states do not have PE designations within specific
disciplines, so the result is many non FPE types that may claim fire
protection as an area of expertise whether qualified or not.

Check out this link to see an outline for what is actually covered on the
NCEES FPE exam

http://www.ncees.org/Documents/Public/PE%20Fire%20Oct%202004.pdf



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Garth W.
Warren
Sent: Wednesday, December 15, 2010 9:41 AM
To: sprinklerforum@firesprinkler.org
Subject: FPE

Does being an FPE necessarily mean that you have training in, or a knowledge

of, fire sprinklers?

Thanks,
Garth 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: FPE

2010-12-15 Thread Jeff Hewitt
When I took the exam in 1995 it was 75%.  I do not know if that is still
accurate.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, December 15, 2010 11:09 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: FPE

Jeff,

What percentage is a passing grade?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, December 15, 2010 12:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: FPE

Garth,

I would say for a legit FPE (Fire Protection Engineer), the answer should be
YES.  However, most states do not have PE designations within specific
disciplines, so the result is many non FPE types that may claim fire
protection as an area of expertise whether qualified or not.

Check out this link to see an outline for what is actually covered on the
NCEES FPE exam

http://www.ncees.org/Documents/Public/PE%20Fire%20Oct%202004.pdf



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Garth W.
Warren
Sent: Wednesday, December 15, 2010 9:41 AM
To: sprinklerforum@firesprinkler.org
Subject: FPE

Does being an FPE necessarily mean that you have training in, or a knowledge

of, fire sprinklers?

Thanks,
Garth 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Ceiling Clouds

2010-12-14 Thread Jeff Hewitt
Tony,

My take is that you are obligated to provide protection at the deck 1st, and
then everything else becomes a potential obstruction to sprinkler discharge
below.  In this case it seems you will also need to drop protection into the
levels of clouds at the 8' level as well.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, December 14, 2010 10:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ceiling Clouds

I agree with going in 15' over a suspended ceiling when the space is open
to another area..., but is that in the code?

A different situation. I have a room about 22 ft. high that has some clouds
for acoustics, at about 15 foot level. These are sprinklered up and down.
There are also some clouds 6 feet in diameter at the 8' level, for mounting
light fixtures. So the difference in height from roof to the 6' dia. Clouds
is about 14 feet. Are sprinklers required below these lower clouds? I should
mention, this is a seismic area, and the clouds are supported with wires
from the roof.

Tony

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: December 14, 2010 8:44 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ceiling Clouds

I don't think so Jimmy.  Up 'til now, the consensus status quo has been to
fully sprinkler up and down but I think a case can be made for going back
15' from the opening in the same spirit as going in 15' over a suspended
ceiling when the space is open to another area ...

SL
 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jimmy Waite
Sent: Tuesday, December 14, 2010 5:52 AM
To: sprinklerforum@firesprinkler.org
Subject: Ceiling Clouds

I know this has been talked about before, but I am having trouble getting
onto the archives.  

I have a situation in an auditorium/lecture hall that has a ceiling that
steps down as you get closer to the front of the room.  However, there is
about a 2'-0 perimeter around the room that is open to the non-combustible
space above the ceiling.  In this case I'd be willing to sprinkle around the
opening (sort of like 8.15.1.5 in the '07), but it seems pointless to
provide coverage over this entire lowered ceiling.  Is there any code that
backs this up? I thought I've heard some, but I don't know where it is.


Thanks,

 Jimmy Waite
 Design Engineer

 jwa...@piedmontfire.com
 mobile: 919.622.7030

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: NICET III

2010-12-08 Thread Jeff Hewitt
I suggest you get your hands on a copy of Sprinkler Hydraulics by Harold Wass
 
 
Jeff Hewitt, PE, SET
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
 
 
 


--- On Wed, 12/8/10, Ron Greenman rongreen...@gmail.com wrote:


From: Ron Greenman rongreen...@gmail.com
Subject: Re: NICET III
To: sprinklerforum@firesprinkler.org
Date: Wednesday, December 8, 2010, 5:39 PM


Read Pat Brock's book. If you understand basic hydraulics the advanced
stuff is just nuance. If you don't understand what you're doing (see
George's post) it will be a mystery and magic. This ain't rocket
science folks--It's just fluid dynamics.

On Wed, Dec 8, 2010 at 3:08 PM, Greg McGahan g...@livingwaterfp.com wrote:
 Where is the least expensive and most beneficial class to prepare for the
 advanced calcs so we cna get his behind us?
 Thanks,
 Greg

 On 12/8/2010 4:56 PM, Bob Knight wrote:

 I'm in the same boat with two left.

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
 McGahan
 Sent: Wednesday, December 08, 2010 2:58 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: NICET III

 What does that do to those of us who only lack one element to pass IV?
 Thanks,
 Greg

 On 12/8/2010 2:23 PM, Art Tiroly wrote:

 Soon the element testing program will not be available. The new test
 is comprehensive pass fail system. Check the NICET website for
 availability - coming soon.


 Arthur Tiroly
 ATCO Fire Protection Design
 Tiroly and Associates
 216-621-8899
 216-570-7030 Cell
 WWW.ATCOfirepro.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
 Mack, SET
 Sent: Wednesday, December 08, 2010 3:20 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: NICET III

 I believe that you need basic hydraulics for III, but you don't need
 to pass Advanced Hyd for III.  You just need that for IV.

 It has been many years since I completed my IV, so I don't recall
 exactly where the breaks are.

 On 12/8/2010 1:19 PM, Brian Harris wrote:

 Am I off my rocker or is it possible to reach NICET III without
 having to take Advanced Hydraulics or Hydraulic Design Area?



 Brian Harris

 First Defense Fire Protection

 11957 Ramah Church Road

 Huntersville, NC 28078

 Phone: 704.948.3506

 Fax: 704.948.3507

 Nicet # 128476







 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16470)
 http://www.pctools.com/ ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 --
 Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road
 Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 --
 Greg C. McGahan Living Water Fire Protection, LLC. 1160 McKenzie Road
 Cantonment, FL 32533 850-937-1850 Fax 850-937-1852
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

RE: Louisiana Professional of Record question

2010-12-01 Thread Jeff Hewitt
Craig,

Sounds like someone has some splainin to do Lucy.

Just because something is done as a design-build project would not somehow
negate the need for a PE.  In fact, just the opposite would hold true.
Design-build implies PE involvement.

In addition, if I was the AHJ, at this point, it is already designed (and
perhaps in for permit and rejected), and now you want to add a PE and come
back with the same design stamped by a PE, I would reject that as well, as
it is obvious the PE just stamped the plans after the fact, and did not do
or supervise the design.

Good luck.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, December 01, 2010 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

What if it was done by a contractor as a design-build project?  No PE
involved.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dale Wingard
Sent: Wednesday, December 01, 2010 8:55 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Craig,

He has to be a PE.  It is normally the Engineer that is part of the original
design of the project.


Dale F. Wingard, SET
Design Manager
Triple A Fire Protection, Inc.
251.649.2034
da...@aaafp.com
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, November 30, 2010 5:22 PM
To: sprinklerforum@firesprinkler.org
Subject: Louisiana Professional of Record question

I need to know from someone who regularly works in Louisiana what the
submittal procedure is if drawings are produced for an owner from an outside
design firm who is not the installing contractor.

Is a POR required to be a PE?

Where are the qualifications listed for the POR in relation to sprinkler
shop drawings?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Louisiana Professional of Record question

2010-12-01 Thread Jeff Hewitt
Regardless of a contractor's intentions, good or otherwise, I have a problem
with this whole process as described.  Getting a PE to stamp something,
AFTER the fact, AFTER it has been already been designed, is NOT KOSHER, or
at least questionable at best, especially if the PE is not
qualified/experienced with fire protection.  This is a violation of the PE
law in most if not all states, and certainly the spirit of the NICET Code of
Ethics as well. 

While it is obvious that Bobby's Company's intentions are good, I am certain
that a LARGE number of contractors out there do not understand the legal
issues involved, and view the need for a PE stamp as just one more obstacle,
one more thing to do to get a permit, just another nuisance cost, and do
exactly what I have described, go and get some PE, any PE that is willing
for a small fee, to stamp their drawings AFTER the FACT.

This is wrong, it is unethical, and illegal for both the PE and the
contractor, and god forbid something happens on one of those jobs, and
everyone gets called to court, or your insurance company finds out.  You
think you're covered, but you're not.  The stamp was obtained illegally, and
therefore your professional liability and errors and omissions coverage is
denied.

This is not another PE vs. layout technician thing. Rather, this is a
statement that if a PE is required, then do it correctly.

Just my 2-cents.  Sorry for the rant, and no offense intended towards Bobby.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Wednesday, December 01, 2010 11:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Lately we have had projects that require us to provide PE stamps. The last
few projects, we were informed after award of contract and before submittal
that we had to have a PE stamp on our drawings. We have a local PE that will
do this, so we send in a change and get him to review and then approve. When
he looks at them he researches the project, design build or not, and makes
sure that everything is done per code before he will sign off. Some of the
projects have a PE on record for the fire protection portion of the project
and still want us to provide a PE stamp before submittal, that's the one
that I do not understand; if they are the engineer of record for the fire
protection on the project, why won't they do like they used to and review
and stamp once it is approved through them? We have even bid a few that
require this in the specs. now - even if the FP portion is engineered from
the beginning.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com

 

 

  _  

From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, December 01, 2010 11:06 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

 

Craig,

Sounds like someone has some splainin to do Lucy.

Just because something is done as a design-build project would not somehow
negate the need for a PE.  In fact, just the opposite would hold true.
Design-build implies PE involvement.

In addition, if I was the AHJ, at this point, it is already designed (and
perhaps in for permit and rejected), and now you want to add a PE and come
back with the same design stamped by a PE, I would reject that as well, as
it is obvious the PE just stamped the plans after the fact, and did not do
or supervise the design.

Good luck.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, December 01, 2010 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

What if it was done by a contractor as a design-build project?  No PE
involved.

Craig L. Prahl, CET  
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dale Wingard
Sent: Wednesday

RE: Louisiana Professional of Record question

2010-12-01 Thread Jeff Hewitt
Bobby,

If your engineer is making changes to your design and is redrawing for
submittal, all the better, but I was not referring to you or your company.
It sounds like you have someone that is qualified to perform these duties,
and do it in a legal and ethical way.

My statement is about this process in general, not about you specifically.  

You cannot tell me that what I described does not occur everyday all over
this country, by those that either do not know, are willing to risk it, or
do not care, and not just in our field of fire protection.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Wednesday, December 01, 2010 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

I disagree.

 

The Arch/Eng and owner require us to get a PE stamp. Yes that does create
another obstacle, but we have a Mechanical (including fire protection) PE
available locally that is used as the FP engineer of record by many
architects on new projects in our area. When it is required, we hire him to
do ours and he wants all of the specs and drawings, as well as the contacts
for all involved. He researches the entire project to make sure that the
fire protection is correct to the application, codes and area - including
other things I am sure I am not aware of. He does his job all the way
through, and at that point he will not stamp our drawings - he creates his
own, calculates them himself and then stamps his drawings. These are now the
drawings that are used for submittal and the project, all the way to
As-Builts. If there are any re-submittals or changes necessary to his
drawings, he does them - all of this is part of his fee. 

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com

 

 

  _  

From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, December 01, 2010 11:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

 

Regardless of a contractor's intentions, good or otherwise, I have a problem
with this whole process as described.  Getting a PE to stamp something,
AFTER the fact, AFTER it has been already been designed, is NOT KOSHER, or
at least questionable at best, especially if the PE is not
qualified/experienced with fire protection.  This is a violation of the PE
law in most if not all states, and certainly the spirit of the NICET Code of
Ethics as well.

While it is obvious that Bobby's Company's intentions are good, I am certain
that a LARGE number of contractors out there do not understand the legal
issues involved, and view the need for a PE stamp as just one more obstacle,
one more thing to do to get a permit, just another nuisance cost, and do
exactly what I have described, go and get some PE, any PE that is willing
for a small fee, to stamp their drawings AFTER the FACT.

This is wrong, it is unethical, and illegal for both the PE and the
contractor, and god forbid something happens on one of those jobs, and
everyone gets called to court, or your insurance company finds out.  You
think you're covered, but you're not.  The stamp was obtained illegally, and
therefore your professional liability and errors and omissions coverage is
denied.

This is not another PE vs. layout technician thing. Rather, this is a
statement that if a PE is required, then do it correctly.

Just my 2-cents.  Sorry for the rant, and no offense intended towards Bobby.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Wednesday, December 01, 2010 11:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Lately we have had projects that require us to provide PE stamps. The last
few projects, we were informed after award of contract and before submittal
that we had to have a PE stamp on our drawings. We have a local PE that will
do this, so we send in a change and get him to review and then approve. When
he looks at them he researches the project, design build or not, and makes
sure that everything is done per code before he will sign off. Some

RE: Louisiana Professional of Record question

2010-12-01 Thread Jeff Hewitt
Chris,

I have not looked, but I would speculate that every state has a similar rule
in their PE laws.  Something to the effect of a PE shall practice only in
their areas of expertise as established by experience, education or
training.

So here's my question, and I would like to see your answer...

How can a PE that is not qualified by training, education, or experience
(any PE, not just an FPE) legitimately claim to provide personal or
immediate supervision over said work?  

 

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Wednesday, December 01, 2010 6:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Maybe it's a definition of design that will help clear this up.  I'm a
little lost at what Jeff takes issue with.  How is any of this different
than a tech, NICET or otherwise, qualified (which is subjective) or not,
putting together a plan and giving it to his boss, the PE, for correction,
comment, improvement and/or signature?  Seems this issue isn't even a FP
issue but a question of all engineering.  Seems to me the design doesn't
exist until the PE signs the drawing and supporting paper (like spec's,
calc's, etc).  A signed drawing is a design everything else up to that point
is?...but random lines on a paper? How the design got to exist is semantics?
Seems there is little difference whether the PE and techs are employed by
the same company.  I once learned the standard ratio is 5 techs per PE (all
engineering not just FPE).  Although I suspect that is a little outdated. 

For example I hereby certify that this plan, specification, or report was
prepared by me or under my direct supervision and that I am a Professional
Engineer under the laws of the State of Minnesota.  Are we talking the
definition of 'direct'?  The MN PE Board ruled on a complaint I filed 10-12
years ago that a PE located MI (and lic in MN) could in fact sign the work
admittedly done here by a non-PE.  I can't quote the exact wording but it
was to the effect they could not rule on the point of direct supervision as
there were nearly infinite ways to accomplish direct supervision.  Once
signed it was then a design qualified by the PE and how it got to exist they
weren't really interested in.   

If you are speaking of SFPE white paper on PE and Tech's role in design
there are few states following this model that I know of.  As a matter of
fact the MN PE board dismissed the PE's role in sprinklers a long time ago. 

I don't consider the MN Board much different than the average Board.  I know
of some better, some worse, certainly don't know all.   

On Bobby's statement He does his job all the way through, and at that point
he will not stamp our drawings - he creates his own, calculates them himself
and then stamps his drawings.  Why, if it's all right?  Sounds like a
marketing issue not an engineering one.  I suppose that is a reason as
justifiable as some others I can't think of. Does he do this as well for any
techs working for him?  Sounds to me like he needs new techs if so.  

Chris Cahill 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, December 01, 2010 11:21 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Bobby,

If your engineer is making changes to your design and is redrawing for
submittal, all the better, but I was not referring to you or your company.
It sounds like you have someone that is qualified to perform these duties,
and do it in a legal and ethical way.

My statement is about this process in general, not about you specifically.  

You cannot tell me that what I described does not occur everyday all over
this country, by those that either do not know, are willing to risk it, or
do not care, and not just in our field of fire protection.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Wednesday, December 01, 2010 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

I disagree.

 

The Arch/Eng and owner require us to get a PE stamp. Yes that does create
another obstacle, but we have a Mechanical (including fire protection) PE
available

RE: Louisiana Professional of Record question

2010-12-01 Thread Jeff Hewitt
Also, you stated Seems to me the design doesn't exist until the PE signs
the drawing and supporting paper (like spec's, calc's, etc).  A signed
drawing is a design everything else up to that point is?...but random lines
on a paper? How the design got to exist is semantics?

I cannot disagree more.  Just because someone went and got a PE, any willing
page stamper to seal their drawing does NOT make it a design at that point.
It is not a legal design if the stamp is not legit, i.e. stamped by a
QUALIFIED PE.  ALL that it means is that they tried to game the system to
get their permit.  How is the public safety served by such abuse?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Wednesday, December 01, 2010 6:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Maybe it's a definition of design that will help clear this up.  I'm a
little lost at what Jeff takes issue with.  How is any of this different
than a tech, NICET or otherwise, qualified (which is subjective) or not,
putting together a plan and giving it to his boss, the PE, for correction,
comment, improvement and/or signature?  Seems this issue isn't even a FP
issue but a question of all engineering.  Seems to me the design doesn't
exist until the PE signs the drawing and supporting paper (like spec's,
calc's, etc).  A signed drawing is a design everything else up to that point
is?...but random lines on a paper? How the design got to exist is semantics?
Seems there is little difference whether the PE and techs are employed by
the same company.  I once learned the standard ratio is 5 techs per PE (all
engineering not just FPE).  Although I suspect that is a little outdated. 

For example I hereby certify that this plan, specification, or report was
prepared by me or under my direct supervision and that I am a Professional
Engineer under the laws of the State of Minnesota.  Are we talking the
definition of 'direct'?  The MN PE Board ruled on a complaint I filed 10-12
years ago that a PE located MI (and lic in MN) could in fact sign the work
admittedly done here by a non-PE.  I can't quote the exact wording but it
was to the effect they could not rule on the point of direct supervision as
there were nearly infinite ways to accomplish direct supervision.  Once
signed it was then a design qualified by the PE and how it got to exist they
weren't really interested in.   

If you are speaking of SFPE white paper on PE and Tech's role in design
there are few states following this model that I know of.  As a matter of
fact the MN PE board dismissed the PE's role in sprinklers a long time ago. 

I don't consider the MN Board much different than the average Board.  I know
of some better, some worse, certainly don't know all.   

On Bobby's statement He does his job all the way through, and at that point
he will not stamp our drawings - he creates his own, calculates them himself
and then stamps his drawings.  Why, if it's all right?  Sounds like a
marketing issue not an engineering one.  I suppose that is a reason as
justifiable as some others I can't think of. Does he do this as well for any
techs working for him?  Sounds to me like he needs new techs if so.  

Chris Cahill 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, December 01, 2010 11:21 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

Bobby,

If your engineer is making changes to your design and is redrawing for
submittal, all the better, but I was not referring to you or your company.
It sounds like you have someone that is qualified to perform these duties,
and do it in a legal and ethical way.

My statement is about this process in general, not about you specifically.  

You cannot tell me that what I described does not occur everyday all over
this country, by those that either do not know, are willing to risk it, or
do not care, and not just in our field of fire protection.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Wednesday, December 01, 2010 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Louisiana Professional of Record question

I disagree

RE: fire caulk sprinkler penetrations

2010-10-06 Thread Jeff Hewitt
Travis,

It's in the IBC code

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: Wednesday, October 06, 2010 11:12 AM
To: sprinklerforum@firesprinkler.org
Subject: fire caulk sprinkler penetrations

  We have a fire marshal that is requesting that the sprinkler head 
penetrations through a rated ceiling be fire caulked.  I thought I read 
somewhere that you are not req'd to fire caulk the fire sprinkler 
penetrations.  If this is correct, can some one point me to the 
code/standard reference for this?

Thanks in advance!

-- 
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Hose Demand

2010-10-05 Thread Jeff Hewitt
Is it actually a private separate water supply, or just a private water main
that is ultimately fed from a public utility source?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, October 05, 2010 2:35 PM
To: sprinklerforum@firesprinkler.org
Subject: Hose Demand

If I have a system with a pump that is fed from a private fire main as
described in 3.8.1.11 (2007) am I allowed to exclude the hose stream from
the calculations per 12.8.2?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Hose Demand

2010-10-05 Thread Jeff Hewitt
I don't see where you get relief from the hose allowance.  It's all from a
city source so it has to be accounted for, somewhere.  You can only squeeze
out so much, and if it is not there, it's not there.  Not including it means
not accounting for it, which is not correct in my opinion.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, October 05, 2010 3:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Hose Demand

This is an addition to an existing building so I can tie the inside hose
valves to the existing system side and not have them in the calc's for the
new side. I was hoping that I could eliminate the 250 outside hose.

Brian Harris
FDFP Inc.
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, October 05, 2010 4:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Hose Demand

Is there any place on the system to take a hose demand?


At 03:54 PM 10/5/2010, you wrote:
Is it actually a private separate water supply, or just a private water
main
that is ultimately fed from a public utility source?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, October 05, 2010 2:35 PM
To: sprinklerforum@firesprinkler.org
Subject: Hose Demand

If I have a system with a pump that is fed from a private fire main as
described in 3.8.1.11 (2007) am I allowed to exclude the hose stream from
the calculations per 12.8.2?



Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476







===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16010)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Control Mode vs. ESFR

2010-09-23 Thread Jeff Hewitt
With most control mode, you have Group A plastic and pallet storage
limitations that you would NOT have with ESFR K14 or K17.  If these are
areas of concern, then that would be an issue.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Thursday, September 23, 2010 3:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Control Mode vs. ESFR

Having issues with an existing job that was laid out using ESFR K17's, it
was mentioned by a local PE that using a Control Mode sprinkler may be the
answer. What are the pro's and con's with using a Control Mode sprinkler in
a warehouse type setting? I've looked at some of the product data sheets and
right away you can see the end head pressure is quite a bit lower than the
ESFR. Are the obstruction rules the same? Etc...

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15940)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Question on sprinklering an attic space

2010-08-20 Thread Jeff Hewitt
Sounds like your consultant is correct in accordance with NFPA 13.  But that
does not address whether there are any specially adopted requirements via
the Department  of Health.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dennis
Schwarzauer
Sent: Friday, August 20, 2010 3:47 PM
To: sprinklerforum@firesprinkler.org
Subject: Question on sprinklering an attic space

I have a single story residential-style structure used for housing
semi-dependent residents for the State Department of Mental Health. The unit
is an Intermediate Care Facility for the Mentally Retarded, but is viewed as
a nursing home by the state agencies.

The building is non-combustible construction; CMU bearing walls with light
gauge metal trusses and standing seam metal roof. The single floor is fully
sprinklered  that is where my problem begins. My boss had me direct the
Consultants to eliminate the sprinkler in the attic, to save money, as the
building was of non-combustible construction. Now the Fire Marshal 
reviewer for the State Health Department are telling me that  all the PVC
vent stacks and piping insulation is non-compliant.

My Consultant is telling me that, as these are concealed spaces, the IBC
allows non-combustible  limited combustible materials to be present without
sprinklers.

Any thoughts?

Thanks,

Dennis M. Schwarzauer

Eley Guild Hardy Architects PA
418 East Capitol Street
Jackson, Mississippi  39201
T 601.354.2572
F 601.355.2006
www.eleyguildhardy.com
P Please consider the environment before printing this e-mail

This email and any files transmitted with it are confidential and intended
solely for the use of the individual or entity to whom they are addressed.
If you have received this email in error please notify us immediately by
replying to the sender and deleting this copy from your system. Please note
that any views or opinions presented in this email are solely those of the
author and do not necessarily represent those of Eley Guild Hardy Architects
PA.  Finally, the recipient should check this email and any attachments for
the presence of viruses. Eley Guild Hardy Architects PA accepts no liability
for any damage caused by any virus transmitted by this email.

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: ESFR Heads

2010-08-03 Thread Jeff Hewitt
The K14 and K17 are the only ESFR with the 32-ft building option.  It is
allowable to utilize the 35-ft. building design criteria instead.

Please be aware that K25 ESFR does not protect the same things that K14 and
K17 do, mainly idle pallets, and uncartoned or exposed Group A Plastics.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, August 03, 2010 2:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads

The ceiling height is right at 32', I'm hoping to be able to use the k...@20
since it will keep the pipe sizes down. However the K25 are about 3 times as
much as the K16.8 


Regards,
Brian Harris
FDFP INC.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 03, 2010 3:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads

Is the ceiling height 32 or 35ft?

It is odd that 32' is the only height that only offers two choices where all
the others offer four choices. 

But both the Handbook and FMDS 2-2 have some comments related to the
selection of sprinklers.  

If you did not have 40-60psi to use for the system and a k...@20 psi for
instance lists its use as applicable to your conditions I can't see any
reason why you could not use a K-25 ESFR sprinkler.  

But understand that a plan reviewer may not accept your alternative since
it's not listed on the chart.  

Per the NFPA 13 Handbook:
The criteria in Table 16.2.3.1 have been expanded to permit broader
applications of ESFR sprinkler technology based on large-scale test results
reviewed by the Technical Committee on Sprinkler System Discharge Criteria.

FMDS 2-2
The K14.0 (K200) pendent, being the original suppression mode sprinkler, has
the widest array of applications.
Do not assume that other suppression mode sprinklers can be used for
applications where the K14.0 (K200) pendent sprinkler is permitted.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, August 03, 2010 9:20 AM
To: sprinklerforum@firesprinkler.org
Subject: ESFR Heads

Quick question about ESFR heads,
In my particular situation I'm using table 16.2.3.1 (pg.150) Storage height
is 25ft, ceiling height is 32ft. Per the table I'm given the choice of
either 14.0k or 16.8k, am I limited to these two options or can I use any
K as long as the data sheets support it?
 
Also,
If it helps the calc's can you go up a level to the 35ft ceiling row and use
those heads?
 
Thanks!
 
 

Brian Harris

 

 


Design Engineer

 

First Defense Fire Protection
11957 Ramah Church Road
Huntersville NC 28078




br...@firstdefensefire.com
www.firstdefensefire.com outbind://80/www.firstdefensefire.com 

 

Ph: 704.948.3506
Fax: 704.948.3507

 

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.18, Virus/Spyware Database: 6.15320)
http://www.pctools.com/ ===

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe

RE: Small Orifice Sprinklers in Water Curtain

2010-07-15 Thread Jeff Hewitt
Steve,

Just thinking out loud, and do not have a copy of 13 in front of me

Aren't closely spaced sprinklers and water curtains listed outside of the
occupancy classification section?  I am not certain that a water curtain
configuration can be classified as Light Hazard, and if it cannot, then
your argument loses validity.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, July 15, 2010 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: Small Orifice Sprinklers in Water Curtain

Scenario: 3-story Light Hazard (Residential) occupancy,
fully sprinklered per 13.

Situation: Exterior exit stairs are too close to glazed
openings in exterior walls and 45-minute window protection is required
(from inside out) for several 2'x3' fixed windows on all three floors.

Challenge:   Can't use window sprinklers because exterior walls
are bearing.   Am proposing to use water curtain provisions of the
building code, and furnish 3 GPM per lineal foot per 13.

 

Question:Since the windows are only 2' wide, and there are
up to 3 windows in a cluster, we will have sprinklers at 4' apart in
several areas and will be provided a baffle of some sort.I can
easily hit my minimum flow rate with small orifice sprinklers and do not
see any restriction in 13 regarding orifice size in a water curtain.
Since it's all Light Hazard, can anyone think of a reason why we can't
use 4.2K pendents?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Small Orifice Sprinklers in Water Curtain

2010-07-15 Thread Jeff Hewitt
Steve,

 

I do not disagree, just wanted to make the point.  Also, if the AHJ accepts
it, that would be another route to take.

 

Jeff Hewitt, PE, SET, SFPE (Professional Member)

Corporate Engineer

Bi-State Fire Protection Corporation

 

241 Hughes Lane

St. Charles, MO  63301

636-946-0011

636-946-5172 (fax)

314-574-6989 (cell)

 

Fire Sprinklers Save lives.

Can You Live Without Them?

 

From: Steve Leyton [mailto:st...@protectiondesign.com] 
Sent: Thursday, July 15, 2010 2:37 PM
To: Jeff Hewitt; sprinklerforum@firesprinkler.org
Subject: RE: Small Orifice Sprinklers in Water Curtain

 

Interesting point, but there is arguably no more nor less fire load at the
perimeter of a residential compartment where the windows occur, so the
hazard group is the same . in theory.

 

Steve Leyton

Protection Design  Consulting

San Diego, CA

 

 

 

From: Jeff Hewitt [mailto:je...@bistatefire.com] 
Sent: Thursday, July 15, 2010 12:26 PM
To: Steve Leyton; sprinklerforum@firesprinkler.org
Subject: RE: Small Orifice Sprinklers in Water Curtain

 

Steve,

Just thinking out loud, and do not have a copy of 13 in front of me

Aren't closely spaced sprinklers and water curtains listed outside of the
occupancy classification section?  I am not certain that a water curtain
configuration can be classified as Light Hazard, and if it cannot, then
your argument loses validity.

Jeff Hewitt, PE, SET, SFPE (Professional Member)

Corporate Engineer

Bi-State Fire Protection Corporation

241 Hughes Lane

St. Charles, MO  63301

636-946-0011

636-946-5172 (fax)

314-574-6989 (cell)

Fire Sprinklers Save lives.

Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, July 15, 2010 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: Small Orifice Sprinklers in Water Curtain

Scenario: 3-story Light Hazard (Residential) occupancy,

fully sprinklered per 13.

Situation: Exterior exit stairs are too close to glazed

openings in exterior walls and 45-minute window protection is required

(from inside out) for several 2'x3' fixed windows on all three floors.

Challenge:   Can't use window sprinklers because exterior walls

are bearing.   Am proposing to use water curtain provisions of the

building code, and furnish 3 GPM per lineal foot per 13.

 

Question:Since the windows are only 2' wide, and there are

up to 3 windows in a cluster, we will have sprinklers at 4' apart in

several areas and will be provided a baffle of some sort.I can

easily hit my minimum flow rate with small orifice sprinklers and do not

see any restriction in 13 regarding orifice size in a water curtain.

Since it's all Light Hazard, can anyone think of a reason why we can't

use 4.2K pendents?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___

Sprinklerforum mailing list

Sprinklerforum@firesprinkler.org

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org

(Put the word unsubscribe in the subject field)



__ Information from ESET NOD32 Antivirus, version of virus signature
database 5282 (20100715) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__ Information from ESET NOD32 Antivirus, version of virus signature
database 5282 (20100715) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Size considerations

2010-05-26 Thread Jeff Hewitt
Thom,

Here's my 2 cents...

I just have to say, I agree in principle with your beef against PE's that
are seemingly unqualified to be writing specs.  I am even OK with issuing
licenses based on disciplines tested.

My problem is this, I do not feel it is acceptable to complain about PE's if
we are not also willing to file complaints against these problem PE's.  In
every state, PE's are a self policing profession.  Each state's regulatory
board relies on the complaint process to investigate license holders.  They
do not have crystal balls to keep an eye on everything.

So as I have stated on this Forum in the past, if you complain about
unqualified PE's you also need to report them to their respective regulatory
agencies for investigation.  If we are not willing to do this, and give the
regulatory agencies the assistance they need to investigate these bad
actors, then we have NO right to complain.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Wednesday, May 26, 2010 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Size considerations

Ok here's my 2cents on 13 as a spec.

NFPA 13 1.1* Scope. This standard shall provide the minimum requirements
for the design and installation of automatic fire sprinkler
systems and exposure protection sprinkler systems covered
within this standard.

So saying Comply with NFPA 13,  edition will allow the contractor to
price the lowest level of protection required, as well as the cheapest
materials allowed.

This is not always in the best interest of the owner.
Take our Gov. for example. They want the buildings they build to last!
Sometimes they want them to withstand explosions or harsh environments. But
generally they are looking for more than the Minimum.

Like you say for 98% of all projects that simple Comply with may work.
But you're missing a very practical financial aspect of the common practice.
That is the owner typically pays the Arch. And Engineer EXTRA for providing
Fire Protection spec. and drawings. I think the going rate is about 1% of
project cost, but I could be wrong on that. Some contracts allow $xxx.xx per
plan sheet and $xx.xx per spec sheet. Since the spec. is already done, and
the drawing doesn't really have to show much, if the responsibility is
shifted to the contractor, this is easy money, and why we see so many ME or
PE's and not FPE's doing this.

I often look at the SFPE's white paper and really find it hard to not lash
out. They are so worried about what NICET Layout techs' are doing they
have just given up on all the PE's who are not qualified to run a 300
machine. Talk about working Outside of their area of Expertise or
Knowledge This is where they should focus. Make every state LIC. FPE's and
all engineers by discipline. Provide grandfathering and comity for anyone
who has a FPE engineering degree and is lic. in another state, but make all
others test.
Whoops, off subject again.

Ok so the reason it's not just do it to 13 is 1) Financial 2)Doesn't have a
ERO unless they require the contractor to supply one. 3)Some owners or AHJ's
want more than 13's minimum design/ materials or? 4) Outside the scope of 13
is one of Rolland's favorite phrases, which to me means Call in the FPE's!
(Like they are some kind of Light Brigade Onward Rode the 300 or some
such.)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Size considerations

2010-05-26 Thread Jeff Hewitt
Yes, you do.  It is not for you to decide or investigate, let the regulatory
agency do their job.  If they get enough similar standard of care or area
of expertise complaints it very well may add up to them taking action.  To
do nothing means nothing will ever happen.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Wednesday, May 26, 2010 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Size considerations

In my case what am I to exactly complain about.  45 pages of really nothing
gives me reason to question IF they are competent.  Especially when their
title is mechanical engineer.  In MN we're not licensed by discipline so
technically no foul.   

Allowing sched 30 pipe gives me another reason to question.  But just
because I've never heard of sched 30 being used, maybe in theory it is
allowed/used elsewhere.

He has a 20k sq.ft. building divided into 2 system.  Not wrong but FM
apparently has gone to unlimited areas but this bus parking facility needs
2?  

One place says OHI and another OHII.  And one could argue large busses
should be EXII for the shielding.  OHI, II or EXII is more a matter of
judgment than a formal violation considering NFPA 13 A.5.3.1 says automobile
parking is OHI.  Granted these ain't automobiles but neither are Suburbans.
And when one reads EXII examples as asphalt saturating that by comparison
sounds worse to me than a bus.  

Listing 6 mfg's or equal of each devices (OSY, check valves...) and with a
few mfg's I haven't heard of gives me reason to question.  Say Venus - fire
sprinklers or Shurjoint Piping Products or GMR International Equipment -
FDC's or Corcoran Piping System - grooved couplings; perhaps they are all
small market folks that really exist.  

Just because in one paragraph he says all piping ...standard weight...then
the next paragraph says wet piping...standard weight or sched 30...makes me
question.  Then the next paragraph says Standard pressure, wet...2 1/2 to
NPS shall be Thinwall galvanized or black steel.  Again questions, it's
all a standard pressure wet system(s). 

All the questions add up to I don't think they are qualified but nothing in
itself is wrong. Do you complain about the not wrong but clearly don't know
sprinklers well enough to be competent? 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Wednesday, May 26, 2010 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Size considerations

Thom,

Here's my 2 cents...

I just have to say, I agree in principle with your beef against PE's that
are seemingly unqualified to be writing specs.  I am even OK with issuing
licenses based on disciplines tested.

My problem is this, I do not feel it is acceptable to complain about PE's if
we are not also willing to file complaints against these problem PE's.  In
every state, PE's are a self policing profession.  Each state's regulatory
board relies on the complaint process to investigate license holders.  They
do not have crystal balls to keep an eye on everything.

So as I have stated on this Forum in the past, if you complain about
unqualified PE's you also need to report them to their respective regulatory
agencies for investigation.  If we are not willing to do this, and give the
regulatory agencies the assistance they need to investigate these bad
actors, then we have NO right to complain.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Wednesday, May 26, 2010 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Size considerations

Ok here's my 2cents on 13 as a spec.

NFPA 13 1.1* Scope. This standard shall provide the minimum requirements
for the design and installation of automatic fire sprinkler
systems and exposure protection sprinkler systems covered
within this standard.

So saying Comply with NFPA 13,  edition will allow the contractor to
price the lowest level of protection required, as well as the cheapest
materials allowed.

This is not always

RE:

2010-04-09 Thread Jeff Hewitt
Yes.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Robert
Thompson
Sent: Friday, April 09, 2010 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: 

was there ever an ordinary hazard group III?  and existing system
designed to ord III  .21/2000  non storage building.
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email rob...@dakotafire.com 

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Seismic Restraint Standards

2010-03-25 Thread Jeff Hewitt
It was also amended by the 2004 IBC Supplement to IBC 2003, and the 2007 IBC
Supplement to IBC 2006

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, March 25, 2010 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Seismic Restraint Standards

What edition of ASCE are you referring to as the latest?To my
knowledge, the 2005 is the latest and sections 13.6.8.2 and 13.6.8.3 speak
directly to the exclusion as you call it.   The 2007 edition of NFPA 13
included revisions, specifically tables 9.3.5.3.2(a) and (b), as well as
Table 9.3.5.6.2 and the associated steps in the calculation procedure, that
meet the prescribed force and displacement requirements of Section 13.3.1
and 13.3.2, if I'm not mistaken.   All that taken together means that a
system designed with seismic bracing in accordance with NFPA 13, 2007 or
2010 editions in fact DOES meet ASCE 7, and in turn the requirements of
Chapter 16 of all IBC editions up to and including 2009.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim Davidson
Sent: Thursday, March 25, 2010 1:37 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Seismic Restraint Standards

TO all;

The IBC refers to ASCE 7 as the Standard for earthquake bracing, if I
remember correctly the ASCE 7 standard in effect at the time of the adoption
of the 2003 IBC specifically excluded NFPA 13 as a standard for earthquake
bracing through the reference in ASCE 7 excluding NFPA 13 seismic bracing
since NFPA 13 requirements did not meet the requirements of  ASCE 7. In the
latest edition of ASCE 7 the NFPA 13 seismic bracing exclusion was removed
from ASCE 7. Be aware of the version of the IBC that is being enforced in
your area of operation since the IBC is considered the legal code which
tells the designer, owner and design professionals what the requirements are
for the building based on occupancy, construction type, ground floor area,
building height and exposure to building.   

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, March 25, 2010 3:46 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Seismic Restraint Standards

We get those cross referenced type specs now and then.

For mechanical piping, plumbing, duct, etc, SMACNA.

For Fire Protection,  NFPA 13. SMACNA isn't referenced in the NFPA
INSTALLATION Standard, because 13 has it's own rules to follow.  

SMACNA is also no longer referenced in the IBC as of the 2003 edition.  ASCE
7 was established as the accepted standard.  However there was some verbiage
placed in the Code which would permit acceptance of other design standards
if approved by the AHJ.

So if the MEOR wants to apply SMACNA to Mechanical piping and duct systems
he needs to request permission from the AHJ to use that standard.

But as previously stated,  NFPA 13 is the applicable standard for design of
seismic bracing for Fire Protection service piping not SMACNA.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Cyr
Sent: Thursday, March 25, 2010 3:01 PM
To: American Fire Sprinkler Association
Subject: Seismic Restraint Standards

Forumites:

General Mechanical specs often refer to SMACNA for seismic restraint of
piping systems. Sprinkler specs often refer to General Mechanical.

Question: Does NFPA 13 seismic bracing requirements take precedence over
SMACNA?

How was the battle won with the MEOR when he says SMACNA is the preferred
standard for bracing of piping systems?

Any comments would be appreciated.

Thank you,
Ed Cyr

*Alpha Fire Sprinkler Corp.*
San Luis Obispo, CA
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field

RE: FM-200 System

2010-03-24 Thread Jeff Hewitt
Hydrogen hydroxide

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker
Sent: Wednesday, March 24, 2010 12:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: FM-200 System

 dihydrogen monoxide

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Wednesday, March 24, 2010 12:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: FM-200 System

I will be robbing this thought some day, nice.  Got to think about putting
it right in our letterhead.  

Sentry Fire - Your Green Contractor - We use only Dihydrogen Oxide, the best
and most environmentally friendly fire fighting agent on the planet.  

Chris 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Wednesday, March 24, 2010 11:46 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: FM-200 System

Just tell the IT guy that the fire protection in his 120 sqft is being
provided by the new wonder chemical di-hydrogen oxide that is cheap,
renewable, safe and is the best fire fighting medium known to man.

On Wed, Mar 24, 2010 at 9:24 AM, John Drucker john.druc...@verizon.net
wrote:
 Adding to Jim's post, here some more critical red flags, all 
 references
to
 2006 IBC/IFC

 Table 503 Notes 1. and 3.; Section 504.2, Allowable height increase 
 due
to
 automatic sprinkler system installation., Section 506.3, Allowable 
 area increase due to automatic sprinkler system installation.

 Table 601 Note e.; An approved automatic sprinkler system in 
 accordance with Section 903.3.1.1 shall be allowed to be substituted 
 for 1-hour fire-resistance-rated construction, provided such system is 
 not otherwise required by other provisions of the code or used for an 
 allowable area increase in accordance with Section 506.3 or an 
 allowable height increase
in
 accordance with Section 504.2. The 1-hour substitution for the fire 
 resistance of exterior walls shall not be permitted.

 Table 1005.1 Egress width per occupant served- With and Without 
 Sprinkler System

 1005.2.1 Two exits or exit access doorways. Exceptions; 2.     Where 
 a building is equipped throughout with an automatic sprinkler system 
 in accordance with Section 903.3.1.1 or 903.3.1.2, the separation 
 distance of the exit doors or exit access doorways shall not be less 
 than one-third of the length of the maximum overall diagonal dimension of
the area served.

 Table 1016.1 Exit Access Travel Distance - With and Without Sprinkler 
 System., Notes b  c; b.        Buildings equipped throughout with an 
 automatic sprinkler system in accordance with Section 903.3.1.1 or 
 903.3.1.2. See Section 903 for occupancies where automatic sprinkler
systems
 in accordance with Section 903.3.1.2 are permitted.
 c.      Buildings equipped throughout with an automatic sprinkler 
 system
in
 accordance with Section 903.3.1.1.

 Table 1017.1 Corridor Fire Resistance Rating - With and Without 
 Sprinkler System; Note c; Buildings equipped throughout with an 
 automatic sprinkler system in accordance with Section 903.3.1.1 or
903.3.1.2 where allowed.

 Hope that helps,

 John Drucker, CET
 Fire Protection Subcode Official
 Fire/Building/Electrical Inspector
 Fire Marshals Office
 Borough of Red Bank, NJ



 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim
Davidson
 Sent: Wednesday, March 24, 2010 11:47 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: FM-200 System

 Remember that the building code requires the building to be 
 sprinklered throughout and the use of alternative fire suppressions 
 systems instead of sprinkler systems does not met the requirements of 
 the building code. Be very careful if the building is classified as an 
 unlimited area building under the building code because the 
 substitution of a clean agent system
for
 the code required sprinkler system would violate the large area 
 building protection requirements of the building code. The owner has 
 no choice but
to
 comply with the building code. I have seen a few building code 
 officials shut down large area buildings because the IT manager had 
 the sprinkler system removed from the IT server room and replaced with 
 a clean agent system. The building code official has the last word 
 when it comes to the building being sprinklered throughout.

 Have a fire safe day!

 Jim Davidson

 Davidson Associates
 Fire Protection * Medical Gas * Code Consulting 302-994-9500   
 Fax:302-234-1781

RE: Extended Coverage Heads Used in Corridor

2010-03-02 Thread Jeff Hewitt
NFPA 13, 2007 11.2.3.3.6 for Room Design Method, and 11.2.3.3.7 otherwise
both stateor when extended coverage sprinklers are installed, all
sprinklers contained within 75 linear feet in the corridor


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Craig
Leadbetter
Sent: Tuesday, March 02, 2010 1:24 PM
To: sprinklerforum@firesprinkler.org
Subject: Extended Coverage Heads Used in Corridor

We have a p[roject where we are using extended coverage sprinkler heads in a
light hazard corridor. What is the least number of heads we would be able to
use in our calculation? 

Craig Leadbetter

Safeguard of Marquette

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: ESFR Spacing NFPA 13 2002 vs. 2007

2009-06-25 Thread Jeff Hewitt
You are allowed to move up to 1-ft. to avoid obstructions to discharge,
either along branch lines, or between lines, but not both at the same time.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ken Holsopple
(forum)
Sent: Thursday, June 25, 2009 12:49 PM
To: sprinklerforum@firesprinkler.org
Subject: ESFR Spacing NFPA 13 2002 vs. 2007

Dear forumites,

I have a situation on a building where have have been contracted to do the
addition. The building is 40'+ at the peak. The existing and new building
are all protected (to be protected) with ESFR. The problem is that the
existing layout consists of several places where the branchlines (running
perp. to the bar joists) are spaced greater than 10'-0. The increased
spacing runs anywhere from 10'-1 to 10'-9. Each of the existing sprinklers
does not exceed the 100 sq. ft. In reading NFPA 13 ('02) Section 8.12.2.2.3
I see that an additional 1'-0 is allowed along the branchline when trying
to miss obstructions created by trusses/barjoists as long as the listed
criteria is met. Note that this only allows moving ESFR ALONG the line. No
mention of increased spacing between lines till you get to Section
8.12.2.2.4. But this section only applies to running parallel with the
steel. I will also note that the equivalent in the 2007 edition expands
8.12.2.2.3 to include wind bracing (what I would call x-bridging and/or
Horizontal Bridging). But it still states that sprinklers can only be moved
along the line. The GC would like us to continue with the spacing of the
original layout. I am resisting. My contention is that no matter what, the
distance between the branchlines should not exceed 10'-0. Am I right in
questioning the additional spacing between the lines or am I being to
literal in my interpretation? 

Best Regards,
Ken Holsopple
Designer 
Rowe Sprinkler Systems, Inc.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: IMC, IPC and nail plates

2009-04-17 Thread Jeff Hewitt
I think you are missing the point.

You have found the references within each Code, but do the Codes apply to
Fire Suppression piping?

Read the SCOPE of each document and you will find that it does NOT include
Fire Suppression piping.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Friday, April 17, 2009 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: IMC, IPC and nail plates


IPC 2006
305.8 Protection against physical damage. In concealed
locations where piping, other than cast-iron or galvanized steel,
is installed through holes or notches in studs, joists, rafters or
similar members less than 1.5 inches (38 mm) from the nearest
edge of the member, the pipe shall be protected by shield plates.
Protective shield plates shall be a minimum of
0.062-inch-thick (1.6 mm) steel, shall cover the area of the pipe
where the member is notched or bored, and shall extend a minimum
of 2 inches (51 mm) above sole plates and below top
plates.

IMC 2006
305.5 Protection against physical damage. In concealed
locations where piping, other than cast-iron or steel, is installed
through holes or notches in studs, joists, rafters or similar members
less than 1.5 inches (38 mm) from the nearest edge of the
member, the pipe shall be protected by shield plates. Protective
shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
steel, shall cover the area of the pipe where the member is
notched or bored, and shall extend a minimum of 2 inches (51 mm) above 
sole plates and below top plates.

Here's how we deal with this. 
We nail plate the sole plates(one or up to 3 depending on the construction,
houses with gypcrete floors typically have an extra plate or two depending
upon how thick the gyp is.) and slip a steel sleeve around the riser coming
thru the plate.(We find we have enough scrap pipe around to keep a constant
supply of 8 sleeves. We use 8 because we have base moldings here that go
to 10 high on occasion.)

Most walls we see are double plates at the top. Only the upper plate is the
actual Top Plate the second plate has a name I forget right now. Any way
we nail plate both plates and have our Nominal 2 below the top plate.
We've never had any problem with doing this from any inspector.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Friday, April 17, 2009 7:59 AM
To: sprinklerforum@firesprinkler.org
Subject: IMC, IPC and nail plates

Had an interesting encounter with an AHJ this week.
He stopped by a jobsite where we're installing CPVC in walls, and found
fault with the nail plates we're using.
I called to follow up on why he didn't like them, and asked for a code
reference. He replied even if it wasn't in the code, he'd enforce nailplates
extending further than ours as a safety issue. So I reminded him that his
authority was to enforce the PA UCC as adopted, not safety issues he took a
personal liking to. 

His code reference arrived by USPS this AM. He cited the IPC and IMC as
applicable to sprinkler piping, which I disagree with.

Any thoughts or previous rulings by other AHJs?

George Church
Rowe Sprinkler

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: IMC, IPC and nail plates

2009-04-17 Thread Jeff Hewitt
Chris,

I respectfully disagree,

IFC 2006 102.7 and 102.8 can only be applied within the overall SCOPE of the
entire IFC document which is limited to Fire Suppression conditions, not
Mechanical, and not Plumbing.  The Scope is found in IFC 2006 101.2

Also, according to IFC 2006 102.6 Referenced Codes and Standards, 

the codes and standards referenced in this code shall be those that
are listed in Chapter 45 and such codes and standards shall be
considered part of the requirements of this code to the prescribed extent of
each such reference.

The commentary to IFC 2206 102.6 states: 

the application of referenced standards is limited to those
portions of the standards that are specifically identified.

Please note that in IFC 2006 Chapter 45, where the reference standards and
codes are listed, IPC 2006 305.8, and IMC 2006 305.5 are NOT specifically
listed/referenced.  


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill
Sent: Friday, April 17, 2009 10:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: IMC, IPC and nail plates

Does our family of codes go into this level of detail?  If not and I don't
think it does, the authority for the AHJ to use what Thom quoted is IFC
102.7 or IFC 102.8.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff Hewitt
Sent: Friday, April 17, 2009 10:40 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: IMC, IPC and nail plates

I think you are missing the point.

You have found the references within each Code, but do the Codes apply to
Fire Suppression piping?

Read the SCOPE of each document and you will find that it does NOT include
Fire Suppression piping.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Friday, April 17, 2009 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: IMC, IPC and nail plates


IPC 2006
305.8 Protection against physical damage. In concealed
locations where piping, other than cast-iron or galvanized steel,
is installed through holes or notches in studs, joists, rafters or
similar members less than 1.5 inches (38 mm) from the nearest
edge of the member, the pipe shall be protected by shield plates.
Protective shield plates shall be a minimum of
0.062-inch-thick (1.6 mm) steel, shall cover the area of the pipe
where the member is notched or bored, and shall extend a minimum
of 2 inches (51 mm) above sole plates and below top
plates.

IMC 2006
305.5 Protection against physical damage. In concealed
locations where piping, other than cast-iron or steel, is installed
through holes or notches in studs, joists, rafters or similar members
less than 1.5 inches (38 mm) from the nearest edge of the
member, the pipe shall be protected by shield plates. Protective
shield plates shall be a minimum of 0.062-inch-thick (1.6 mm)
steel, shall cover the area of the pipe where the member is
notched or bored, and shall extend a minimum of 2 inches (51 mm) above 
sole plates and below top plates.

Here's how we deal with this. 
We nail plate the sole plates(one or up to 3 depending on the construction,
houses with gypcrete floors typically have an extra plate or two depending
upon how thick the gyp is.) and slip a steel sleeve around the riser coming
thru the plate.(We find we have enough scrap pipe around to keep a constant
supply of 8 sleeves. We use 8 because we have base moldings here that go
to 10 high on occasion.)

Most walls we see are double plates at the top. Only the upper plate is the
actual Top Plate the second plate has a name I forget right now. Any way
we nail plate both plates and have our Nominal 2 below the top plate.
We've never had any problem with doing this from any inspector.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Friday

RE: PODs storage again

2009-03-30 Thread Jeff Hewitt
Ron, 

it's better not to use hangers on this one, put it under water.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Monday, March 30, 2009 4:37 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: PODs storage again

I think the consensus was to hang the building for from a fusible link
over a pond.

Is it a new building? If so it would be interesting to see what the EOR
or architect did for a hazard analysis.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
Mack, SET
Sent: Monday, March 30, 2009 2:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

I tried to search the archives, but keep getting a file not found error.
I
am looking at a PODs storage warehouse.  There was a lot of discussion
on
the forums a while back, but I can't access all of it.  The facility I
am
looking at has 24' storage.  
 
What is the general concensus of the protection req'd for these areas?
 
Thanks in advance for your help.
 
 
 
Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Seismic - NFA 13 vs. IBC

2009-03-19 Thread Jeff Hewitt
Ken,

I disagree.

The requirements for the 2-in. clearance is to prevent damage to the
sprinkler or drop due to excessive movement of the piping, not the due to
movement of the ceiling.  If the ceiling is held to a more strenuous
standard making it more rigid, that will not remove the requirement for the
2-in. clearance.

However, I do agree with you that these are separate issues.  Being able to
utilize NFPA 13 to satisfy ASCE 7 and the IBC for seismic bracing
requirements is separate entirely from whether those drops need the
additional 2-in clearance protection mandated by ASCE 7 or IBC.

I personally do not agree with this provision for 2-in clearance located in
ASCE 7, and thus the IBC, since NFPA 13 already has allowances/requirements
for branch line restraint, which apply to hard ceilings, but not your
everyday typical mineral type acoustical ceiling panel, as described in the
commentary of NFPA 13 on this topic.  The ASCE 7 and IBC documents make no
clarification on this.  At least for this issue, there seems to be a lack of
consistency.

Just my 2-cents.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
ParsleyConsulting
Sent: Thursday, March 19, 2009 2:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Seismic - NFA 13 vs IBC

Rich,

I think the supplement provides a great deal of clarification, if what 
Joe Powell's question dealt with was Does the IBC allow NFPA-13 
criteria to be used for seismic protection. 

I understand your reference regarding the oversize rings, but I think 
it's relevant to note that the section you're quoting is a part of 
ceiling requirements, not seismic protection of sprinkler systems, with 
one exception.  Item (e) in 13.5.6.2.2 requires the 2 oversize ring for 
sprinkler penetrations in ceilings which are not rigidly braced (see the 
exception to item (b)).  Information we've received suggests that 
ceilings in seismic design categories D-E-F are going to be required by 
ASTM C635 and ASTM C636 are going to require rigid bracing of the 
ceiling components, which would eliminate the need for the 2 oversize 
ring. 

The important distinction here is that the ASCE7 reference is not for 
rigid bracing of the drops to the sprinklers, but rather to the ceiling 
itself. 
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax

R Richardson wrote:
 Even with the new language in the supplement as referenced by Steve, 
 the issue is not clear.

 The language in the supplement indicates that NFPA 13 is essentially 
 equivalent to section 13.6.8 of ASCE.

 However, the requirement for 2 in. oversized rings is not in section 
 13.6.8. It is in section 13.5.6.2.2, and that section still speaks to 
 sprinkler heads thought suspended ceilings needing 2 in. rings.

 Not that I am an advocate of the 2 in. ring, we haven't really even 
 enforced it yet thinking it was going to go away, but it seems to 
 still be required.

 Rich Richardson
 Seattle Fire Department

 Steve Leyton st...@protectiondesign.com 03/13/2009 13:29 
 I call Jeff a little while ago to thank him for that post; if you have
 interest in this issue, there is free download at ICC's web site (you do
 not have to be a member).

 http://www.iccsafe.org/cs/codes/2007-08cycle/2007Supplement/IBC07S.pdf

 The clarification is in new section 1613.6.3, page 128 of the supplement
 (page 132 of the PDF).

 Steve Leyton
 Protection Design  Consulting
 San Diego, CA

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: CEILING CLOUDS - AGAIN

2009-02-06 Thread Jeff Hewitt
Travis,

Since we have no specific guidance on this topic, my recommendation is that
you must protect to deck first, and deal with the obstructions second.

With this criteria, I would recommend both above and below the clouds.

Just my thoughts

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: Friday, February 06, 2009 3:50 PM
To: sprinklerforum@firesprinkler.org
Subject: CEILING CLOUDS - AGAIN

I have a project with lots of floating clouds.  The clouds slope with the
roof deck and are 1' below the roof deck.  If I place a sprinkler in the
cloud, is one req'd in the space above the cloud?  I would normally put
sprinklers above the clouds, but with the deflector already at 12 below the
roof deck based on the cloud height, do you really need the sprinklers above
the clouds?
 
Please feel free to call if you have any questions or comments.
 
Travis Mack, SET
 mailto:tm...@mfpdesign.com 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Sprinklered vs Sprinkled

2009-01-14 Thread Jeff Hewitt
kinda like nuclear vs nucular

--- On Wed, 1/14/09, bill.bro...@brooksfpe.com bill.bro...@brooksfpe.com 
wrote:

From: bill.bro...@brooksfpe.com bill.bro...@brooksfpe.com
Subject: Sprinklered vs Sprinkled
To: sprinklerforum@firesprinkler.org
Date: Wednesday, January 14, 2009, 10:47 PM

Actually this is a serious question.

Is there anywhere in the country where the term sprinkled is
commonly
used by sprinkler industry types to describe a building with a sprinkler
system?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: solid unit load examples

2008-12-23 Thread Jeff Hewitt
Dewayne,
 
We did a job a few years ago for a landscape block manufacturer.  They used a 
solid plastic skid/tray/pallet, call it what you want, it was 4 inches this, 
and solid plastic.  They stacked these in an accumulation area and recycled 
them back thru the automated process.  The accumulation area needed protection 
for solid unit load of Group A plastics.  Along these lines I am sure you can 
use your imagination and come up with some others, such as plastic/plexiglass 
sheets stacked solid just like drywall, or similar arrangements.  Each 
situation would need to be evaluated to come to an agreement whether the 
storage configuration was a solid unit load.
 
just my 2 cents..
 
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)

--- On Tue, 12/23/08, Dewayne Martinez deway...@dbfp.net wrote:

From: Dewayne Martinez deway...@dbfp.net
Subject: solid unit load examples
To: sprinklerforum@firesprinkler.org
Date: Tuesday, December 23, 2008, 11:05 AM

Could I please get some examples of a solid unit load of nonexpanded
plastics?
I am having trouble picturing a load that does not have any voids (air)
within the load.
Thanks,
Dewayne
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Fire Pump Controller

2008-12-08 Thread Jeff Hewitt
Joe,

Try this:

NFPA 70, 2005 edition, 695.6 (F) Junction Points.  

Where wire connectors are used in the fire pump circuit, the connectors shall 
be listed.  A fire pump controller or fire pump power transfer switch, where 
provided, shall not be used as a junction box to supply other equipment, 
including a pressure maintenance (jockey) pump.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Monday, December 08, 2008 10:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Fire Pump Controller

I just had a job site meeting with a electrical contractor. He stated the 
engineer wanted to feed the jockey pump controller from the fire pump 
controller. Something about a tapping rule or exception. I cautioned against 
it, told him to research it first. Can anyone give me a section that prohibits 
this arrangement from either NFPA 20 or NEC? 

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: design and coordination roles and responsibilities.

2008-11-12 Thread Jeff Hewitt
That's a good story!!

PE's like that deserve to be cut off at the knees.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, November 12, 2008 2:42 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: design and coordination roles and responsibilities.

My favorite story in the ongoing battle between the professionals is the 
difficulty Steve Leyton had with a registered PE who informed him that 
by the virtue of his lack of registration as a PE that he was 
unqualified to discuss the issues related to standpipe design, use, 
and compliance with NFPA-14.  The fact that Steve was a member of the 
NFPA-14 committee at the time escaped the notice of the individual, and 
in a delicious moment of irony Steve pointed to his name in the front of 
the book. 

That was a day I'll long cherish.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website



Ron Greenman wrote:
 Once I was called incompetent by the architect because in the field
 there was one inch of clear space between the bottom of the beams in a
 parking garage and the minimum low clearance for the cars and I
 couldn't fit a four inch pipe in the space (and I couldn't touch the
 beams. He drew nine inches but the excavator screwed up, the garage
 got poured and it was my problem somehow.

 On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon [EMAIL PROTECTED]
wrote:
   
 Your RIGHT! Because the sprinkler contractor is now the only one that
does
 his layout in 3D he visualizes all of the problems the others call Field
 Conditions.
 Architects get really pissed off when you point out that they and their
 consultants didn't co-ordinate space above the ceiling even with their
own
 structural engineer. Yeah the ceiling to bottom of floor is 36, and
there
 are recessed lights in the ceiling with lenses that make them 8 deep.
And
 yes you clearly show the 16x30 duct, and the cable tray and our main is
only
 6, so what's your problem? COULD IT POSSABLY BE THAT W30 beam we're all
 shown crossing?

 Since ancient times the builder of empires and Architects have had the
same
 theory, KILL the messenger!!

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926


 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
 - FPDC
 Sent: Wednesday, November 12, 2008 10:59 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: design and coordination roles and responsibilities.

 One of the consistent problems we have up here is the electrician.
 They don't take part in the coordination process, they often don't even
have
 CAD drawings and they just run everything where they want.
 And the GC's tend to let them get away with a lot of it. I find that more
 problems with the architect's concepts surface in the sprinkler design
that
 any of the other trades.


 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 



   
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: White papers and definition of roles

2008-11-10 Thread Jeff Hewitt
Very narrow minded Craig.  Do you actually believe that Sprinkler System
installation is ALL that there is in the FPE realm?

I would say now what I have said in the past.  If you have had a bad
experience with a so called PE practicing fire protection, turn them in to
the appropriate state regulating agency/board.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, November 10, 2008 1:13 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: White papers and definition of roles

I've held the position that no one should receive a PE license until they've
actually worked in the field as an installer or helper for a contractor in
their respective field for at least two years.

I've seen far too many young engineers given responsibility over projects
just because of those letters when they knew nothing more than a collection
of calculation methods.  But corporations, lawmakers and others foster the
idea that 4+/- years of book learnin', time as EIT, and pass the test to get
those letters, earns you the title of Expert.  So we suffer with that
misguided definition of expert.

Over the years it has been obvious which PE's (fire prot and others) have
never been to the construction site to see their creation first hand.
Trying to convince someone that just because you can draw it doesn't mean it
can be built is one of the greatest challenges.

Having worked for both Mechanical and Fire Protection contractors, dealing
with Engineers was often the most difficult part of the project.



I have learned to appreciate FPE's like Jim Roberts for his mentoring
attitude and investment in the people he works with.  Thanks!


Craig L. Prahl, CET
Lowly Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, November 07, 2008 1:09 PM
To: sprinklerforum@firesprinkler.org
Cc: sprinklerforum@firesprinkler.org;
[EMAIL PROTECTED]
Subject: Re: White papes and definition of roles

Ken,

I have been saying this for years.

Within my large organization, I get frustrated with PEs (and non-Fire
Protection PEs) thinking they know fire protection.

We've since reorganized in Greenville and don't have a separate department,
but at one time we had up to 27 fire protection  auxiliary systems
engineers and designers.  I insisted that our engineers get their Level IIIs
- minimum.

In looking at resumes and conducting interviews, I was more interested in
people who realized that no one is an expert in all aspects of fire
protection, or for that matter automatic sprinklers systems.  If someone
claims it, watch out!

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





[EMAIL PROTECTED] ParsleyConsulting Sent by:
[EMAIL PROTECTED]
11/07/2008 12:44 PM
Please respond to sprinklerforum

To
sprinklerforum@firesprinkler.org
cc

Subject
Re: Fire Pump Suction







Steve, that's what makes that idiotic best-of-all-possible-worlds white
paper on the role of the PE and the designer so funny.

It makes two assumptions which are absolutely brainless.  First that there
are enough PE's to do all that work, and second, that those same PE's
actually know what they're doing.

I used to be in awe of those two little letters, until a very proud of
himself PE informed me that the appropriate remote area in a military BOQ
was the 300' long hallway, which was 5'-0 wide, thus resulting in a 1,500
square foot remote area.

On that day I became aware that those letters by themselves don't convey
competence.  What a pity.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website



Steve Leyton wrote:
 I wonder how many projects out there have been scrambled like eggs by
 the EOR ...

 Steve Leyton
 Protection Design  Consulting
 San Diego, CA


 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Todd
 Williams - FPDC
 Sent: Friday, November 07, 2008 6:27 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Fire Pump Suction



 Sadly I hang my head when I hear where was the EoR.

 John Drucker
 Fire Protection Subcode Official (AHJ) New Jersey


 I wonder how may projects there are out there with no EoR?

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, Connecticut
 www.fpdc.com
 860.535.2080

RE: White papers and definition of roles

2008-11-10 Thread Jeff Hewitt
Thank you Thom,

That is my point exactly.  The PE profession is self policing.  Regulating
boards will not and cannot act unless someone files a complaint.  Let them
look into it, that's their job, but by all means FILE the COMPLAINT.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Monday, November 10, 2008 3:05 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: White papers and definition of roles

As with most things in life, people only do what they have too, to get by.
PE's are no exception, only if they are held to a standard they cannot
comply with will they respond by doing what is necessary to meet that level
of competence. Many states don't even have continuing education
requirements. At least NICET got that part right.
Lic. By specialty, continuing education, and a higher level of competence
won't happen without someone complaining about what is happening now. Don't
fix what isn't broke, is the rule most Quasi Gov. bodies live by. If you
want it to change YOU WILL have to make it happen! PE's that don't know ESFR
from SSP, will continue as they are, unless someone speaks up.
As George would say Just say NO! to people working outside their area of
expertise.


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



On a complaint they have to prove competence you do not have to prove
incompetence. This is especially true in States where PE's are general and
not licensed by specific testing.  For example I passed the fire protection
PE exam.  With the PE I can sign civil drawings IF I have training and
experience in such issues.  I do not have to take the CE exam.  If ever
called before the board I'd have problems because I have no training or
experience in CE matters.  Perhaps there are others with FP and CE training

and experience that could sign both legally by passing the EE test.   


Chris Cahill, P.E.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: ESFR Heads below obstructions

2008-11-05 Thread Jeff Hewitt
Just curious

If you have NO intentions of listening to the good advice you are getting
here on this forum, why ask the question to begin with?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Wednesday, November 05, 2008 7:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

It has nothing to do with competiveness. 

I'm not a contractor. 

It is a matter of replacing a public supply with A 1500gpm pump and 350cum
Tank. 

Not a small change. 

Dan

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 05 November, 2008 3:34 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

Really?  Two heads will keep you from being competitive?  That must be some
real close bidding.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, November 05, 2008 8:25 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

If you add the flow of two additional heads below obstructions you won't be
low bid. The added flow will probably drive your main sizes up a pipe size
and it may affect the fire pump as well.

It isn't all that dissimilar to storage racks. We know if racks with solid
shelves are added to a warehouse the flow for the in-rack sprinklers would
have to be added into the roof calc yet we don't make an allowance for them
in the shell system, at least we don't.

Around here TI contractors chop up ESFR systems by adding heads at demising
walls and under ducts but they don't do a new roof system calc.
I would bet that 8 out of 10 ESFR systems in Phoenix don't calc after TI but
AHJ's around here either don't care or more likely don't know.

Ron Fletcher
Aero Automatic
Phoenix, AZ


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 2:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

Well, I read all that and it seems that all you need are 12 heads

Dan


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 04 November, 2008 7:28 PM
To: sprinklerforum@firesprinkler.org
Subject: ESFR Heads below obstructions

Dan,

All references here are from the '07 edition of NFPA-13:

14.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

15.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of  the levels shall be
included with those of the other level in the hydraulic calculations.

16.2.3.5 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations

16.3.3.6 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

17.2.3.4 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

17.3.3.5 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

22.4.4.6.4 The requirements of 22.4.4.6.1 to include every sprinkler in the
design area to be included in the system discharge shall not apply; where
ESFR sprinklers are installed above and below obstructions, the discharge
for up to two sprinklers from one of the levels shall be included with those
of the other level in the hydraulic calculation.

Based on what I read in the ROP just published it doesn't look like any of
these have been removed, although it appears that the wording in
22.4.4.6.4 has been moved around a bit, and a new 22.4.4.6.4.1 has been
added (See 13-462, Log CP82 in the ROP)

Hope that is what you were after.
*
*PARSLEY CONSULTING

Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website

RE: ESFR Heads below obstructions

2008-11-05 Thread Jeff Hewitt
So, that makes it ok, then?

You know better, but you go ahead and do it wrong anyway?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, November 05, 2008 7:25 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

If you add the flow of two additional heads below obstructions you won't
be low bid. The added flow will probably drive your main sizes up a pipe
size and it may affect the fire pump as well.

It isn't all that dissimilar to storage racks. We know if racks with
solid shelves are added to a warehouse the flow for the in-rack
sprinklers would have to be added into the roof calc yet we don't make
an allowance for them in the shell system, at least we don't.

Around here TI contractors chop up ESFR systems by adding heads at
demising walls and under ducts but they don't do a new roof system calc.
I would bet that 8 out of 10 ESFR systems in Phoenix don't calc after TI
but AHJ's around here either don't care or more likely don't know.

Ron Fletcher
Aero Automatic
Phoenix, AZ


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 2:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

Well, I read all that and it seems that all you need are 12 heads 

Dan


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 04 November, 2008 7:28 PM
To: sprinklerforum@firesprinkler.org
Subject: ESFR Heads below obstructions

Dan,

All references here are from the '07 edition of NFPA-13:

14.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of the levels shall be 
included with those of the other level in the hydraulic calculations.

15.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of  the levels shall be 
included with those of the other level in the hydraulic calculations.

16.2.3.5 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations

16.3.3.6 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

17.2.3.4 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

17.3.3.5 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

22.4.4.6.4 The requirements of 22.4.4.6.1 to include every sprinkler in 
the design area to be included in the system discharge shall not apply; 
where ESFR sprinklers are installed above and below obstructions, the 
discharge for up to two sprinklers from one of the levels shall be 
included with those of the other level in the hydraulic calculation.

Based on what I read in the ROP just published it doesn't look like any 
of these have been removed, although it appears that the wording in 
22.4.4.6.4 has been moved around a bit, and a new 22.4.4.6.4.1 has been 
added (See 13-462, Log CP82 in the ROP)

Hope that is what you were after.
*
*PARSLEY CONSULTING

Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website



danarbel wrote:
 Question regarding the number of ESFR heads required for hydraulic
calc. 

 The nominal number is 12. 

 There was a requirement to add 2 heads if there are heads installed
below
 beams or AC ducts. 

 If I'm not wrong the addition of 2 heads was abolished. 

 Please confirm or correct me,

 Dan Arbel


 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to:
[EMAIL PROTECTED]

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 No virus found in this incoming message.
 Checked by AVG - http://www.avg.com 
 Version: 8.0.138 / Virus Database: 270.8.6/1765 - Release Date:
11/3/2008
4:59 PM


   

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL

RE: ESFR Heads below obstructions

2008-11-05 Thread Jeff Hewitt
Travis,

I understand the position that you are trying to explain from others, but I
have to disagree with the premise.

This is suppression mode protection, NOT control mode protection.  All
research and testing has clearly indicated that ESFR protection is very
sensitive to obstructions.  I still shake my head in amazement at the
attempts by some to justify doing something less.

We DO include an allowance for additional ESFR heads in our calcs, up front,
and it's amazing, we still manage to compete, while doing the right thing.
To me it's a cop out.  

As to the comment Why calculate the system to 14 heads if the tenant never
has additional heads due to obstructions or other items?  I have yet to see
an ESFR system that did not have obstruction issues requiring additional
heads at some point.  I don't think we (collectively) are being honest about
this if we believe otherwise.

Just my 2 cents.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack,
SET
Sent: Wednesday, November 05, 2008 10:16 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

I think what Ron is implying is that the shell system is designed for one
thing, but the tenant later comes in and puts in solid shelves or adds heads
under ductwork.  The original system was designed, reviewed, approved,
installed, inspected and accepted per NFPA and local requirements.  When the
TI contractor comes in later down the road (1 day - 10 years later, who
knows), they often do not do the due diligence to calculate the extra heads
under obstructions.

If a contractor is to bid a shell system with 14 heads flowing vs 12 heads,
they may as well not even bid.  You have bigger pipes and possibly a bigger
pump.  While 14 may be the prudent thing to do, you have to also go with
practical.  Why calculate the system to 14 heads if the tenant never has
additional heads due to obstructions or other items?

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Wednesday, November 05, 2008 9:08 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

So, that makes it ok, then?

You know better, but you go ahead and do it wrong anyway?

Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State
Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, November 05, 2008 7:25 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

If you add the flow of two additional heads below obstructions you won't be
low bid. The added flow will probably drive your main sizes up a pipe size
and it may affect the fire pump as well.

It isn't all that dissimilar to storage racks. We know if racks with solid
shelves are added to a warehouse the flow for the in-rack sprinklers would
have to be added into the roof calc yet we don't make an allowance for them
in the shell system, at least we don't.

Around here TI contractors chop up ESFR systems by adding heads at demising
walls and under ducts but they don't do a new roof system calc.
I would bet that 8 out of 10 ESFR systems in Phoenix don't calc after TI but
AHJ's around here either don't care or more likely don't know.

Ron Fletcher
Aero Automatic
Phoenix, AZ


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 2:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Heads below obstructions

Well, I read all that and it seems that all you need are 12 heads 

Dan


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 04 November, 2008 7:28 PM
To: sprinklerforum@firesprinkler.org
Subject: ESFR Heads below obstructions

Dan,

All references here are from the '07 edition of NFPA-13:

14.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations.

15.4.4 Where ESFR sprinklers are installed above and below obstructions,

the discharge for up to two sprinklers for one of  the levels shall be
included with those of the other level in the hydraulic calculations.

16.2.3.5 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one of the levels shall be
included with those of the other level in the hydraulic calculations

16.3.3.6 Where ESFR sprinklers are installed above and below obstructions,
the discharge for up to two sprinklers for one

RE: Fire Pump Suction

2008-11-04 Thread Jeff Hewitt
Dan,

That is incorrect information.  This is still a requirement in NFPA 13.
Some had previously reported that FM was planning to remove it from the FM
Data Sheet requirements.  Someone was confused, as it has not, nor was it
ever planned to be removed.  In fact, as currently worded, the FM
requirement could lead to including MORE than 2 additional heads in an ESFR
remote area.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 10:51 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Pump Suction

Question regarding the number of ESFR heads required for hydraulic calc. 

The nominal number is 12. 

There was a requirement to add 2 heads if there are heads installed below
beams or AC ducts. 

If I'm not wrong the addition of 2 heads was abolished. 

Please confirm or correct me,

Dan Arbel


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Attic Question

2008-10-29 Thread Jeff Hewitt
Will NFPA 13, 2007, 8.15.1.5 work for you?

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis
Sent: Wednesday, October 29, 2008 2:14 PM
To: sprinklerforum@firesprinkler.org
Subject: Attic Question

I have searched the archives and can not find an answer. I am working on a
detention center that is of steel, block and concrete construction. The
attic area has insulation right under the roof. There is a concrete walkway
where we will be placing electric HVAC units. My question is do I have to
sprinkle the entire attic, and would it need to be dry, or should I have
them enclose the walkway and just sprinkle the mech room?

Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Mezz design area

2008-10-29 Thread Jeff Hewitt
I would be careful stating that the entire mezzanine is an obstruction to
the overhead deck sprinkler protection, and you don't have to calculate it.
That is not a valid argument.  This is a separate area.  What pipe sizing
are you going to use?  What will you base that on?  There are many
unanswered questions here.  The NFPA 13 standard states that you do not have
to include heads added due to obstructions to the hydraulic calculations,
for a head or two here and there, but to apply it to an entire 50 x 50
mezzanine is a BIG stretch.  Just my 2 cents

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, October 29, 2008 3:45 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mezz design area

Assuming both are the same occupancy, which area is going to be your
hydraulically remote, the roof or under the mezzanine?  Is the use on or
under the mezzanine different than the use of the open floor area?

If the roof is your hyd. remote area then the mezzanine is just an
obstruction and you don't need to calculate it if the design criteria is the
same as the roof.

If they are different occupancies then they are different zones.

What bearing does a stair opening in the middle of a 100K sf building have
on the design area?  It's a floor opening, just don't run your pipes through
it.  LOL

Adjust your remote area to include the required number of heads for the
calcs.  The remote area isn't always a perfect rectangle.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, October 29, 2008 4:34 PM
To: sprinklerforum@firesprinkler.org
Subject: Mezz design area

I think we've talked about this before but couldn't come up with anything in
the archives.



Roof elv. just over 20'.  All quick response heads.



50' x 50' mezzanine in a corner so that one 50' side is open to above.  This
situation also comes when you have a hole in a first floor open to the
second.



At the roof the design area is 1500 but what about under the mezz?



I tend to lean to a full 1500 sq.ft. under the mezz. but that's just
conservatism and I don't think it's really supported in code either way.
Even if the wall is around all 4 sides you might have a stair opening
wrecking the reduced remote area if that's otherwise allowed.



What about a two story 1,000,000 sq.ft. building with a 33.34' x 30' stair
opening in the middle?  I can see doing by the opening 1500 sq.ft. but what
is by the opening mean.  How far away until you are no longer near.



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: [EMAIL PROTECTED]



Mail: P.O. Box 69

Waverly, MN 55390



Location: 4439 Hwy 12 SW

  Waverly, MN 55390



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pesticides Storage

2008-10-16 Thread Jeff Hewitt
Ray,

NFPA 30 or even 30B if you have any aerosols is a good place to start.  If
you don't find anything to your liking, you may also want to review the
applicable FM Data Sheets on Flammable and Combustible Liquids to see if
they have a protection scheme to match your situation.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Thursday, October 16, 2008 10:30 AM
To: sprinklerforum@firesprinkler.org
Subject: Pesticides Storage

Esteemed Collegues:

Can anyone give guidance on a Pesticides Storage warehouse and the
approriate fire protection requirements?
NFPA-434 doesn't give prescriptove requiremetns or a definitive path to
follow. It only indicates a risk analysis be done by a competent
individual (I read PE or FPE) to determine the extent and type of fire
protection to be provide.

Without regard to storage arrangement and heights, what TYPE of commodity
would be appropriate to consider, since the amount stored is over 10,000 lbs
and is extermely varied in the types and configurations of products to be
stored?
I am leaning towards NFPA-30 Flammable and Combustible Liquids to begin my
analysis, but would like the opinions of anyone who has had experience with
this process.

Thanks in advance,

Ray Vance -SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.comblocked::blocked::http://www.waynefire.com/
(407) 877-5563  office
(321) 436-2184  cell

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Mattress stroage

2008-08-07 Thread Jeff Hewitt

Andy,

Be careful with this one.  It seems to me that the storage as described 
would constitute Uncartoned (Exposed) Expanded Group A Plastics (NOT Class 
IV), which have VERY limited applicability for ESFR.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.



- Original Message - 
From: Andy Johnston [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Thursday, August 07, 2008 1:28 PM
Subject: Mattress stroage


I am working on a bid for a warehouse. I was given a floor plan for the new
building and a copy of the fire plan from the same building they just
finished in another state.

The also sent photos of the existing building.



The pics show mattress in plastic bags staked on end all lined up in a row.
Just like in dramatic burn video I recently watched.

The other area of the warehouse has couches bagged the same way. Sitting on
12'3 bay racks.

The sprinkler plans for the this are list it as Class IV commodity protected
with EFSR heads and no in rack system.



Even if they put the stuff back in the boxes I can't see how they a class V
commodity

Is there some thing I am missing before I call the engineer?



Thank you for your attention.

Andy Johnston

Andy Johnston

Master Craft Plumbing Contractors Inc. Phone (386)252-7047 Fax (386)898-0322


Your are welcome to call my Cell (386)547-4970



The information contained in this transmission is privileged and
confidential. No reader may make any use of it's contents with out the
written approval of the sender. The recipient should not act or use the
information in this transmission or any of its attachments without separate
authentication of its authenticity or approval.  If you have received this
in error I apologize please notify me so I can correct my records. Thank you
for your cooperation.










___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Floating Ceilings

2008-08-05 Thread Jeff Hewitt
I have been watching this thread with interest, and finally have to ask (and 
yes, I am sure this will stir the pot as well)


This particular issue is one which requires more than just mundane 
interpretation of the NFPA 13 standard.  Who should be doing the 
interpreting???  NICET technicians, or PEs, or ???


My gut feeling here is that if you choose to support the more liberal 
interpretation, that this will NOT require both above and below protection, 
especially without any significant test data to back it up at this point, 
that this is not the place for a NICET technician to make this decision, or 
for that matter to try to sell it to the local AHJ.  Do you really want 
that liability?  Not to mention whether you are exceeding your authority 
under NICET rules for practicing engineering?





Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.




- Original Message - 
From: Rick Green [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, August 05, 2008 10:38 AM
Subject: RE: Floating Ceilings


NFPA 13 2002 Edition - Section 8.14.1.2.2 - Noncombustible and limited 
combustible concealed spaces with limited access and not permitting 
occupancy or storage or combustibles shall not require sprinkler 
protection.  The space shall be considered a concealed space even with 
small openings such as those used as return air for a plenum.


Maybe I did not describe correctly the ceiling construction.  The ceiling 
will be installed throughout the space(s) at the same elevation.  The 
openings are 7 gaps along the perimeter walls or between sections of 
the ceiling within the room.  This only occurs in a few of the 
spaces/rooms and those rooms are separated by full height wall from other 
spaces.


I believe the section above may adequately address this issue to the point 
I can meet with AHJ concerning sprinkler protection above the ceiling 
space.





___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Floating Ceilings

2008-08-05 Thread Jeff Hewitt
As a PE, lacking any further guideance or test data to make any sort of 
engineering judment or equivalency argument, NFPA 13 only gives you one 
obvious interpretation.  In my opinion, based on the situation described, it 
is not a concealed space, therefore sprinklers may not be omitted above the 
ceiling, and I would not entertain any offers to make a contrary judgement.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Russell [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, August 05, 2008 12:23 PM
Subject: RE: Floating Ceilings



As a PE, what approach would you take if faced with this situation?



Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130



My gut feeling here is that if you choose to support the more liberal
interpretation, that this will NOT require both above and below 
protection,

especially without any significant test data to back it up at this point,
that this is not the place for a NICET technician to make this decision, 
or

for that matter to try to sell it to the local AHJ.  Do you really want
that liability?  Not to mention whether you are exceeding your authority
under NICET rules for practicing engineering?




Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Floating Ceilings

2008-08-05 Thread Jeff Hewitt
Pardon me for making some suggestions to add to your decision making 
process.


You did indeed bring the issue to the forum, and you got several angles to 
think about, including mine.  Far too many times the aspects that I 
mentioned are not considered.  I simply pointed them out to you.


Is the forum an appropriate place for a negative response such as yours?

No one was questioning your authority to ask the forum for insight to make 
themselves feel better.  Perhaps you should re-read the post.  As for 
bravado?  There are others on this forum than just you, that may appreciate 
others' perspectives on issues such as this.


I make NO apologies for this.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Rick Green [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org; Rick Green [EMAIL PROTECTED]
Sent: Tuesday, August 05, 2008 12:50 PM
Subject: Re: Floating Ceilings


I bring this issue like others to the forum for a place to throw out ideas 
hoping for feedback


I believe it is important in a forum environment to share ideas with 
others who have experienced similar situations


My earlier comments were provided so forum members know what my brain is 
thinking


My interpretation is based on reading the code and comments from NFPA 
specific as I could get to the issue.  No,  I did not complete fire tests 
or call my local PE for an answer before starting this thread.  I did not 
know this forum required such high a threshold


Feel free to question my authority to ask the forum for insight if that 
makes you feel better.  I know that bravado  provides absolutely no value 
to the forum


Sincerely,

Exceeding my authority but thankful for the  forum
--Original Message--
From: Jeff Hewitt
To: sprinklerforum@firesprinkler.org
ReplyTo: sprinklerforum@firesprinkler.org
Sent: Aug 5, 2008 12:24 PM
Subject: Re: Floating Ceilings

I have been watching this thread with interest, and finally have to ask 
(and

yes, I am sure this will stir the pot as well)

This particular issue is one which requires more than just mundane
interpretation of the NFPA 13 standard.  Who should be doing the
interpreting???  NICET technicians, or PEs, or ???

My gut feeling here is that if you choose to support the more liberal
interpretation, that this will NOT require both above and below 
protection,

especially without any significant test data to back it up at this point,
that this is not the place for a NICET technician to make this decision, 
or

for that matter to try to sell it to the local AHJ.  Do you really want
that liability?  Not to mention whether you are exceeding your authority
under NICET rules for practicing engineering?




Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by 
one

or more legal privileges.  It is intended solely for the use of the
addressee identified above.  If you are not the intended recipient, any 
use,
disclosure, copying or distribution of this e-mail is unauthorized.  If 
you

received this e-mail in error, please notify the sender immediately at the
above captioned address.



- Original Message -
From: Rick Green [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Tuesday, August 05, 2008 10:38 AM
Subject: RE: Floating Ceilings



NFPA 13 2002 Edition - Section 8.14.1.2.2 - Noncombustible and limited
combustible concealed spaces with limited access and not permitting
occupancy or storage or combustibles shall not require sprinkler
protection.  The space shall be considered a concealed space even with
small openings such as those used as return air for a plenum.

Maybe I did not describe correctly the ceiling construction.  The ceiling
will be installed throughout the space(s) at the same elevation.  The
openings are 7 gaps along the perimeter walls or between sections of
the ceiling within the room.  This only occurs in a few of the
spaces/rooms and those rooms are separated by full height wall from other
spaces.

I believe the section above may adequately address this issue to the 
point

I can meet with AHJ concerning sprinkler protection above the ceiling
space.




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http

Re: Sprinkler Pattern Obstructions

2008-07-14 Thread Jeff Hewitt

Brian,

I believe it should be read to mean that the most/furthest away you have to 
be is a maximum of 36-in.  The 36-in. is the maximum limit.  Without this 
provision, you would instead need to be 4 times away or 96-in.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 1:36 PM
Subject: Sprinkler Pattern Obstructions



Forum,
I know I must be reading this wrong but as usual I am in a hurry and could
use some help. NFPA-13 (2007) 8.8.5.2.1.3 states that the sprinkler shall 
be

positioned a minimum of 4 times the maximum dimension of the obstruction,
but then it goes on to say a maximum of 36 clear space. In my case I have 
a

24 column I'm trying to avoid which by the 4 times rule would get me 8'
away, how does the max. 36 clear come into play? Also look at Figure
8.8.5.2.1.3, I'm so confused 


Regards,


http://www.firstdefensefire.com/








E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/








___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Sprinkler Pattern Obstructions

2008-07-14 Thread Jeff Hewitt

Brian,

NFPA 13, 2007 8.8.5.2.1.3 states...the maximum clear distance required (for 
extended coverage UR/Pendent heads) shall be 36-in..


What needs to be clarified?

This already is clarified from previous editions.

I think it's pretty clear.

36-in. is the MAXIMUM, regardless of the actual 4 times dimension.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 2:18 PM
Subject: RE: Sprinkler Pattern Obstructions



Jeff,
That's the confusing part, how can 36 work when the book also says it 
needs

to be 96? I think some clarifying in the next release may be in order.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Monday, July 14, 2008 2:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler Pattern Obstructions

Brian,

I believe it should be read to mean that the most/furthest away you have 
to

be is a maximum of 36-in.  The 36-in. is the maximum limit.  Without this
provision, you would instead need to be 4 times away or 96-in.


Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer 
Bi-State

Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by 
one

or more legal privileges.  It is intended solely for the use of the
addressee identified above.  If you are not the intended recipient, any 
use,
disclosure, copying or distribution of this e-mail is unauthorized.  If 
you

received this e-mail in error, please notify the sender immediately at the
above captioned address.
- Original Message -
From: Brian Harris [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 1:36 PM
Subject: Sprinkler Pattern Obstructions



Forum,
I know I must be reading this wrong but as usual I am in a hurry and
could use some help. NFPA-13 (2007) 8.8.5.2.1.3 states that the
sprinkler shall be positioned a minimum of 4 times the maximum
dimension of the obstruction, but then it goes on to say a maximum of
36 clear space. In my case I have a 24 column I'm trying to avoid
which by the 4 times rule would get me 8'
away, how does the max. 36 clear come into play? Also look at Figure
8.8.5.2.1.3, I'm so confused 


Regards,


http://www.firstdefensefire.com/








E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
5.10250e http://www.pctools.com/en/spyware-doctor-antivirus/









___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/





E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Sprinkler Pattern Obstructions

2008-07-14 Thread Jeff Hewitt

Brian,

Sorry,

I don't see it that way.  It does not say that this only applies to 
obstructions up to 9-in wide or your up a creek.


What it does say is that if you are 36-in away that is all the further you 
need be.


Contact me by phone to discuss this.  I am in the office.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 2:48 PM
Subject: RE: Sprinkler Pattern Obstructions



Jeff,
Basically the 4 times rule is only good for obstructions up o 9 wide 
then,

why not just make 36 the number and be done with it?


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Monday, July 14, 2008 3:40 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler Pattern Obstructions

Brian,

NFPA 13, 2007 8.8.5.2.1.3 states...the maximum clear distance required 
(for

extended coverage UR/Pendent heads) shall be 36-in..

What needs to be clarified?

This already is clarified from previous editions.

I think it's pretty clear.

36-in. is the MAXIMUM, regardless of the actual 4 times dimension.



Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer 
Bi-State

Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by 
one

or more legal privileges.  It is intended solely for the use of the
addressee identified above.  If you are not the intended recipient, any 
use,
disclosure, copying or distribution of this e-mail is unauthorized.  If 
you

received this e-mail in error, please notify the sender immediately at the
above captioned address.
- Original Message -
From: Brian Harris [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 2:18 PM
Subject: RE: Sprinkler Pattern Obstructions



Jeff,
That's the confusing part, how can 36 work when the book also says it
needs to be 96? I think some clarifying in the next release may be in
order.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Monday, July 14, 2008 2:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler Pattern Obstructions

Brian,

I believe it should be read to mean that the most/furthest away you
have to be is a maximum of 36-in.  The 36-in. is the maximum limit.
Without this provision, you would instead need to be 4 times away or
96-in.


Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected
by one or more legal privileges.  It is intended solely for the use of
the addressee identified above.  If you are not the intended
recipient, any use, disclosure, copying or distribution of this e-mail
is unauthorized.  If you received this e-mail in error, please notify
the sender immediately at the above captioned address.
- Original Message -
From: Brian Harris [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, July 14, 2008 1:36 PM
Subject: Sprinkler Pattern Obstructions



Forum,
I know I must be reading this wrong but as usual I am in a hurry and
could use some help. NFPA-13 (2007) 8.8.5.2.1.3 states that the
sprinkler shall be positioned a minimum of 4 times the maximum
dimension of the obstruction, but then it goes on to say a maximum of
36 clear space. In my case I have a 24 column I'm trying to avoid
which by the 4 times rule would get me 8'
away, how does the max. 36 clear come into play? Also look at Figure
8.8.5.2.1.3, I'm so confused 


Regards,


http://www.firstdefensefire.com/








E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
5.10250e http://www.pctools.com/en/spyware-doctor-antivirus/




--
--




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field

Re: ESFR Sprinklers over 8' library shelves

2008-06-23 Thread Jeff Hewitt

Mark,

What about maintaining adequate flue spaces, and no solid shelves?  It 
sounds like your bin boxes/shelf units have neither, ragardless of storage 
height.  150,000 sq.ft. is an fairly large area for something that doesn't 
really conform to the intent of ESFR protection.  Are you maybe thinking 
this is an ordinary hazard occupancy, and ESFR is allowed over OH 
occupancies?



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Phelps, Mark [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, June 23, 2008 3:23 PM
Subject: RE: ESFR Sprinklers over 8' library shelves


Joe,
Thanks for the response. To give you a little more detail, the shelf units 
are approximately 14 deep by 4' wide with 5 shelves high to 6'. The 
shelving is all sheet metal with solid backs and ends. The shelves are 
arranged in rows, back to back, and share a common divider, (like double row 
racks without a longitudinal flue). They have 4' aisles and are open on the 
top shelf. This storage arrangement occupies an area of about 150,000 square 
feet in a building that encloses 500,000 square feet. There are 2 X 4 foot 
light fixtures, AC ductwork up to 26 inches in diameter and banks of conduit 
up to 3 in diametter and over 2' wide through-out the ceiling space of this 
building.
To clarify your second paragraph, when you refer to meet the obstruction 
rules, I assume you mean these obstructions at the roof, as I have just 
discribed, and not the shelves themselves?

Thanks again,
Mark at Aero


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Joe
Hankins
Sent: Friday, June 20, 2008 7:21 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: ESFR Sprinklers over 8' library shelves


Mark,

First and foremost, this is  an application  that (due to what I presume
are solid shelves) takes advantage of  none of ESFRs strengths but is
subject to all of their weaknesses.  Unless these shelves are in a small
area of a facility that is otherwise a good fit with ESFRs, ESFRs are
the wrong choice.

If the ESFR protection is already existing and the shelves meet all
definitions of shelf storage, then you are OK as long as you meet the
obstruction rules.

The bottom line is that, in order for suppression to reliably occur, you
have to meet the obstruction rules, regardless of storage height. While
lowering the storage height makes a fire easier to suppress, increasing
the clearance makes it harder. The solid shelves further exacerbate the
challenge.

Joe




Phelps, Mark wrote:
Mr. Joe Hankins, If you are on line, could you comment on the application 
of ESFR (K14 at 75 PSI) installed below a 40' high roof protecting class I 
thru IV misc storage on library style shelves (not an actual library). My 
specific question is,  do all of the design requirements and obstruction 
requirements (conduit banks, lights, ducts, etc.) and exceptions apply 
equally as if it were double row racks of I thru IV stored to 30'?

Mark at Aero
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Max flow for class I standpipes

2008-05-29 Thread Jeff Hewitt

Fully sprinklered building, 1000-gpm max. for standpipes.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Dewayne Martinez [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Thursday, May 29, 2008 4:12 PM
Subject: Max flow for class I standpipes


What is the max flow for class I standpipes in a fully sprinklered
building?  I have 4 in a building and have been taught in the past to
only calculate 1000 gpm max (7.10.1.1.3, NFPA 14 (03 ed)) but section
7.10.1.2.3 seems to contradict this.
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: NFPA13 Dwelling vs Mercantile

2008-05-15 Thread Jeff Hewitt

Russell,

My take is that if you are using residential heads, and residential head 
design criteria, then the 3000 sq.ft area does not apply because you are not 
utilizing an area/density design.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address. 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Corrosion Resistant Concealed Sprinkler Plate

2008-04-22 Thread Jeff Hewitt

Bobby,

I hope this works for your application.  Besides corrosion, our concern was 
with hot water and steam eventually eroding any wax coating.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Bobby McCullough [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, April 22, 2008 9:08 AM
Subject: RE: Corrosion Resistant Concealed Sprinkler  Plate


Jeff:

I received an off forum response from Globe.  Their concealed model 5604
(old style stair step cover) is listed as corrosion resistant when
manufactured with the polyester coating.  When you order this, just
specify (very clearly) that you want a white poly sprinkler with wax
touch-up installed in the cup.

Bobby

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Wednesday, April 16, 2008 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Corrosion Resistant Concealed Sprinkler  Plate

We recenly went through this for a USDA application in a clean room for
meat
cutting, where hot water and steam are used to clean up every day,
causing a
corrosive environment to exposed sprinkler heads.

We looked, and no such animal exists.  The closest you can get is an
MRI
room head that is non-ferrous brass, with a plastic concealer housing,
but
still no corrosion resistance listing on it.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by
one
or more legal privileges.  It is intended solely for the use of the
addressee identified above.  If you are not the intended recipient, any
use,
disclosure, copying or distribution of this e-mail is unauthorized.  If
you
received this e-mail in error, please notify the sender immediately at
the
above captioned address.


- Original Message - 
From: Bobby McCullough [EMAIL PROTECTED]

To: SprinklerFORUM@firesprinkler.org
Sent: Wednesday, April 16, 2008 8:24 AM
Subject: Corrosion Resistant Concealed Sprinkler  Plate


Does anyone know of a concealed sprinkler and plate with a corrosion
resistant finish?  I have a spec requiring this sprinkler over a pool.

Thanks,

Bobby McCullough
Allsouth Sprinkler Company678-730-4312
[EMAIL PROTECTED]


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Failed Bucket Test

2008-04-07 Thread Jeff Hewitt

Brian,

Just curious...

What were the circumstances that led you to use a test conducted by the Fire 
Department?  Are there conservation limitations imposed or something like 
that?  Why would you not have performed your own test?


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, April 07, 2008 1:51 PM
Subject: RE: Failed Bucket Test



Chuck,
Yeah that was one of the first things we did, we also had the local 
Utility

Dept. go out and check and they found nothing.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chuck 
Bowman

Sent: Monday, April 07, 2008 2:42 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Failed Bucket Test

Brian,
Has anyone checked to make sure all the valves are fully open, just a
suggestion.
Chuck

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian 
Harris

Sent: Monday, April 07, 2008 2:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Failed Bucket Test

Fellow forum people:
I have a situation where we have designed and installed a 13R system, it 
is

completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns out
that a test taken now with the failed test shows a 25% drop in static 
residual pressures, hence the failed test. Of course the owner is looking 
to

us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a
few different things but with that big of a pressure loss there's really 
not
much we can do. I don't feel it's our liability at this point since we 
went

off the city's water flow test and per the calc's we were good, any
thoughts?


Regards,


http://www.firstdefensefire.com/








E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/





E-mail message checked by Spyware Doctor (5.5.0.178)
Database version: 5.09560
http://www.pctools.com/spyware-doctor/
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Do you look up?

2008-04-04 Thread Jeff Hewitt
Todd,
   
  Without getting into specific cases, I have turned in more than 15 on the 
consulting/specifying side.  I have had no negative experiences from this.  All 
complaints are addressed by the state, and they send letters explaining any 
actions taken or agreed to.
   
  I also have a rubber stamping problem in my area, and it is not limited to 
Fire Protection.  I am fortunate to have an active Regulating Board here in 
Missouri.
   
  In all cases, the State was not aware there was an alleged problem, until the 
complaint was filed.  They do the investigating, they do the follow up.  Our 
job is to let them know.
  
Todd Williams - FPDC [EMAIL PROTECTED] wrote:
  Jeff,

You, as a PE on staff with a contractor is very much the exception, 
rather then the rule, especially in this part of the planet. Off 
hand, I can only think of one contractor in CT with a PE on staff and 
that is because it is a family business and the son went to school 
specifically to do that. As an independent, the only time I am 
invited back is if there is a significant enough change that someone 
thinks I need to address it, or it is required for sign-off by the 
AHJ. Fortunately, most of my clientele are focused on doing the job 
right so in the installations I have seen I rarely see obvious problems.

Just out of curiosity, how many PE's have you 'turned in'? My total 
is one. Never heard anything back from anyone.

Todd


At 11:17 PM 4/3/2008, you wrote:
Again, sorry for the late response, I'm away from the office.

 Todd,

 while it was off of my point, let me answer your question 
 directly, how many times has an installer changed my 
 drawings? NONE!! Not once without my knowledge and blessing. I 
 set the standards for my company, our drawings and installations 
 are completed under my supervision as a licensed engineer, and our 
 fitters do not make changes without asking first, they know better 
 than to try. And yes, I do check my company's installations. And 
 yes, I realize that I am an exception. I am not a consultant for 
 hire, but rather a full time employee of ONE contractor, beholden 
 to that contractor only.

 I think you have directed my comments off point. I realize and 
 agree that there is plenty of blame to go around, from specifying 
 PE's to Layout techs and installers. Don't get me started on that tangent.

 My comments are specifically directed at those repeated 
 complaints about unqualified engineers that show up on this forum 
 from time to time. I understand the frustrations involved, I have 
 to deal with them myself. Installers and layout techs creating 
 problems is one thing, but PE's, we're talking about licensed 
 professionals here. If they're not qualified, they need to be 
 cited and stopped. Same as doctors and other regulated 
 professions. No excuses. gather your evidence and turn them 
 in. My experience has been that it does not take much for most of 
 them to wake up when the Regulating Board comes calling.

 I realize you were addressing the installations, but Mark did 
 play the PE card.

Todd Williams - FPDC wrote:
 The complaint here is not about the engineering, but the
installation. We are talking about what is physically in the
building. You're a PE, Jeff; how many times has an installer changed
your drawings? My guess is a lot. I know in my situation, I am rarely
asked to certify an installation once it is complete. I don't hold up
anybody's money and I don't hold up the CO. Then the last eyes for
seeing the job was done right is the AHJ. If it is not caught there,
that's how it remains. The fault may well be with the specifying
engineer (if there is one), but it may lie elsewhere.


At 10:07 PM 4/2/2008, you wrote:
 Sorry for the late reply to Mark's comments, I've been travelling all day.
 
  I saw this and felt compelled to repeat my previous thoughts on
  this issue. Mark's comments bring me to a statement that I have
  made on here before, and I will likely again, the next time this comes up.
 
  You cannot just complain about this PE issue. Turn them
  in!! There is no other way. Their regulating Boards can do
  nothing without a complaint, and for that matter thay will NOT even
  know about it, unless WE speak up and do something about it.
 
  Yes, that's right, an engineer telling you to turn in a fellow
  engineer. I will not defend anyone that claims this or anything
  else as an area of expertise when they are not actually qualified.
 
  Turn them in! And don't get fed up if nothing happens right
  away. Their investigations may take a while.
 
  Again, rather than seeing all of these complaints about inept
  specifying engineers, let's all do something different now, or it
  will only get worse.
 
  Gather your facts, file the complaint, and turn them in.
 
 
  Jeff Hewitt, PE, SET, MSFPE (Professional Member)
  Corporate Engineer
  Bi-State Fire Protection Corporation
  St. Charles, MO 63301
 
 Mark Sornsin wrote:
  When I look up at work

Re: Gaggle of closets

2008-02-22 Thread Jeff Hewitt

Chris,

Don't be so quick to jump to that conclusion.  Another case of it says this 
or it doesn't say that so I can do it.  I think you should be very careful 
here.  Dig a little deeper and get to the logical intent, and not just what 
it says or doesn't say in black and white.


This is an area separate from the dwelling areas, and is likely to be 
crammed full of who knows what.  In addition, there is no mention of wall or 
ceiling contruction (which could affect one's direction on this issue).


I agree with Greg that this is not likely what the NFPA standard committee 
intends for this exception.


In reading the commentary in the Automatic Sprinkler Systems Handbook on 
this issue, I believe there is merit to the fact that the standards 
committee intended small rooms to mean small light hazard/low fuel load 
rooms.  This would not seem to be low fuel loading, and is not, in my 
opinion, is an ordinary hazard area rather than light hazard.  And because 
it's storage, and you don't know what could go in there, OH1 ain't good 
enough, it needs to be OH2.


Just my opinion



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Chris Mak [EMAIL PROTECTED]

To: sprinklerforum sprinklerforum@firesprinkler.org
Sent: Friday, February 22, 2008 4:40 PM
Subject: Re: Gaggle of closets


Could you foresee a fire senario where the 47 extra heads would operate.  I 
think that this is exactly what the exception is for.


Regards


- Original Message -
From: Paul Pinigis [EMAIL PROTECTED]
Sent: 22/02/2008 05:30 PM EST
To: sprinklerforum@firesprinkler.org
Subject: RE: Gaggle of closets



Don't you just love it when the letter of the code works in your favor.
I really don't think that this is what the NFPA 13 committee had in mind
when they developed that section.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, February 22, 2008 5:05 PM
To: sprinklerforum@firesprinkler.org
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according
to NFPA 13. On the first level, there is a room which contains 55 -
3'x5' tenant storage closets (mostly filled with shelves). These
would need to be sprinklered, which is fine, but the issue comes in
the hydraulics. Section 14.4.4.4.2 states that closets with a single
sprinkler may be omitted from the calculation. There could be up to
47 closets in the remote area. I have used this exception numerous
times, but never in this quantity. The standard says nothing to the
contrary, so I could eliminate 47 sprinklers in the remote area
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


This document should only be read by those persons to whom it is addressed 
and is not intended to be relied upon by any person without subsequent 
written confirmation of its contents. Accordingly, our company disclaim all 
responsibility and accept no liability (including in negligence) for the 
consequences for any person acting, or refraining from acting, on such 
information prior to the receipt by those persons of subsequent written 
confirmation.


If you have received this e-mail message in error, please notify us 
immediately by telephone. Please also destroy and delete the message from 
your computer. The Unsolicited Electronic Message Act 2007 (The Spam Act) 
came into effect from 5 September 2007. As a valued client you may receive 
communications from us from time to time, including electronic publications, 
invitations and related information. Please advise if you wish us to stop 
sending these communications to you. Otherwise we will assume you wish to 
continue receiving these communications from us.


Any form

Re: Delta Flows

2008-02-19 Thread Jeff Hewitt

Why so touchy Brian???

Looks to me like Cliff was offering to help you out.

You're the one requesting help, a little more gratitude would go a long way, 
lest some of us decide it's not worth the effort, if that's the response 
we'll get.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, February 19, 2008 10:35 AM
Subject: RE: Delta Flows



Cliff,
Why are you so quick to cut somebody down? I thought this forum was here 
to

help each other. If you must know the individual that holds our license is
one of the most highly rated contractors in this industry, he is on 
vacation

and I don't think this is a life or death situation that warrants me
interrupting that. I just got a phone call from another highly qualified
forum member that agreed with my solution, thanks for your time.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, February 19, 2008 11:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Delta Flows

Brian,

Apparently the person in your office that is qualified to hold your
contractor's license is out of pocket or he could help you solve the
problem.  Contact me off-forum with a phone number where I can call you 
and

I will see if I can help.  If you can email me your dwg file, it will help
speed things up.

Cliff Whitfield, SET
Fire Design, Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian 
Harris

Sent: Tuesday, February 19, 2008 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: Delta Flows

I am working on a job and the calc's are kicking my butt! My most 
demanding

head has a delta flow of 0, which makes sense, but allot of the other
heads in the remote area are overflowing by up to 10! The calc of course
doesn't work, it's 40 pounds over, I've tried everything I know. Any help
would be appreciated.


Regards,


http://www.firstdefensefire.com/





___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Delta Flows

2008-02-19 Thread Jeff Hewitt



Am I missing something here??  I have re-read Cliff's post an do not see the 
phrase bought it anywhere.


As for someone directing this comment towards me that all those 
abbreviations after your name were bought, not earned. , I would simply 
shrug it off, as I know my abilities, and the person making those comments 
obviously knows nothing about me, but is entitled to their opinion, 
incorrect though it may be.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, February 19, 2008 12:50 PM
Subject: RE: Delta Flows



Am I the only one that read he was suggesting that our qualified license
holder bought it? Read his post again and tell me you wouldn't get
offended if someone said all those abbreviations after your name were
bought, not earned.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Tuesday, February 19, 2008 1:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Delta Flows

Why so touchy Brian???

Looks to me like Cliff was offering to help you out.

You're the one requesting help, a little more gratitude would go a long 
way,

lest some of us decide it's not worth the effort, if that's the response
we'll get.


Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer 
Bi-State

Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by 
one

or more legal privileges.  It is intended solely for the use of the
addressee identified above.  If you are not the intended recipient, any 
use,
disclosure, copying or distribution of this e-mail is unauthorized.  If 
you

received this e-mail in error, please notify the sender immediately at the
above captioned address.
- Original Message -
From: Brian Harris [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Tuesday, February 19, 2008 10:35 AM
Subject: RE: Delta Flows



Cliff,
Why are you so quick to cut somebody down? I thought this forum was
here to help each other. If you must know the individual that holds
our license is one of the most highly rated contractors in this
industry, he is on vacation and I don't think this is a life or death
situation that warrants me interrupting that. I just got a phone call
from another highly qualified forum member that agreed with my
solution, thanks for your time.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Tuesday, February 19, 2008 11:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Delta Flows

Brian,

Apparently the person in your office that is qualified to hold your
contractor's license is out of pocket or he could help you solve the
problem.  Contact me off-forum with a phone number where I can call
you and I will see if I can help.  If you can email me your dwg file,
it will help speed things up.

Cliff Whitfield, SET
Fire Design, Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, February 19, 2008 9:04 AM
To: sprinklerforum@firesprinkler.org
Subject: Delta Flows

I am working on a job and the calc's are kicking my butt! My most
demanding head has a delta flow of 0, which makes sense, but allot
of the other heads in the remote area are overflowing by up to 10! The
calc of course doesn't work, it's 40 pounds over, I've tried
everything I know. Any help would be appreciated.


Regards,


http://www.firstdefensefire.com/





___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send

RE: Wet Manual Standpipe

2008-01-22 Thread Jeff Hewitt
Tom,
   
  NFPA 14, and IBC 2003 and 2006 have all been updated to clarify the intent 
here. 
   
  It IS acceptable to use a manual wet standpipe, in NON HIGH RISE buildings, 
whwere there is not enough pressure for the standpipe demand, but an adequate 
supply for JUST sprinklers is provided, making use of the standpipe system to 
supply a comination system.  The Fire Department pumper is considered to be the 
fire pump for the standpipe demand, vis the FDC.
   
  That being said, I can see providing a fire pump just large enough to feed 
the sprinkler demand only.  
   
  This assumes all other facets are there, adequate supply for suction for 
pumper to provide standpipes, etc...I have seen many cases where there was 
adequate volume for standpipe demand, but not pressure, and the pressure and/or 
volume were adequate for the sprinkler system.
   
  So, in my opinion, the engineer does not have his b**ls in a vise.
   
  Jeff Hewitt, PE, SET, MSFPE (Prof. Member)
  Bi-State Fire Protection Corporation
  St. Charles, MO  63301

Tom Duross [EMAIL PROTECTED] wrote:
  I always thought if you install a pump to feed a standpipe and spkrs, it had
to feed the standpipe and spkrs.
I've seen some odd installations where the pump was only sized to meet the
sprinklers.
Some engineer has his b**ls in a vise in my opinion.
If you don't have the supply to satisfy a pump to satisfy the standpipe, why
install the pump?
Get a variance.
TD


Absolutely it can be done.

If there is not enough water to supply the standpipes with a pumper truck,
then there isn't enough water to feed it with a fixed pump and there is a
secondary problem. But in practical application it is common down here to
use a small pump for the system and use manual wet standpipes in low-rise
buildings.

In fact; didn't someone on the NFPA #14 committee said that it was never the
intent for a fixed pump to solely satisfy the standpipe requirements without
assistance from the local Fire Department? Or did I imagine this?

Greg

Is there enough water to supply the pump? Are there hydrants to supply the
fire truck and standpipes with adequate water?

Art @ ATCO Fire

Can this be done and is there any value?? Local water pressure is pitiful.
Provide wet manual standpipes (2), sprks need max 250 GPM at 40 PSI so use a
250 at 40 pump and there is an emergency generator which can connect to this
small pump. We save money on the pump, pipe sizes are reduced and the wet
manual meets code for a 4 story hotel. Anyone ever do this?? Thanks in
advance.


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: When a Spec is a Spec...

2008-01-21 Thread Jeff Hewitt

Brian,

I think you write a clearly worded RFI, requesting clarification that the 
drawings are for intent only, and not necessarily for head placement.  I 
think it also depends on who is taking engineer of record responsibilities.


We prefer to take engineer of record responsibilities, and via RFI, make any 
changes we wish, within the intent of NFPA 13, as long as hydraulics back it 
up.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Brian Harris [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Monday, January 21, 2008 1:12 PM
Subject: When a Spec is a Spec...


How do most of you interpret when a spec or notes on the FP drawings 
specify

that the max. head spacing is not to exceed 130 sq.ft. but you have plenty
of water/pressure to go extended coverage. Do you go e.c.? Stay 2 130 max,
call the GC?


Regards,

 http://www.firstdefensefire.com/












___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Seismic Bracing and 2002 NFPA 13 Appendix

2008-01-18 Thread Jeff Hewitt

Tom,

I feel that this should be clarified further.

My understanding, at least as affected by the ICC Codes, is as follows:

The 2003 edition of IBC removes the reference to the use of NFPA 13 from 
ASCE 7 2002 edition. (The version of NFPA 13 referenced is NFPA 13, 1999, 
NOT NFPA 13 2002).  NFPA 13, 2002 TIA 02-1 was the fix for this snub, but 
IBC never actually issued a formal interpretation or Supplement judgement 
stating that.


The 2006 edition of IBC does not have the same verbage removing NFPA 13 that 
IBC 2003 did, and also uses the NFPA 13, 2002 edition as the reference 
document, NOT NFPA 13, 1999, but does add other stipulations for its use.


The 2007 Supplement to the 2006 IBC removes all remaining hurdles by simply 
adding a new section to the IBC 2006 Earthquake provisions, allowing the use 
of NFPA 13 , with no other stipulations.  Please note that the NFPA 13 2002 
version is STILL the reference document to IBC 2006, NOT NFPA 13, 2007.


There is currently no version of IBC that references NFPA 13 2007.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Thom McMahon [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Friday, January 18, 2008 12:43 PM
Subject: Re: Seismic Bracing and 2002 NFPA 13 Appendix


Remember that if your spec. requires you to meet ASCE 7 requirements that 
NFPA 13, 2002 was found not to meet these, however 2007 was accepted as 
substantially meeting these requirements. Also there was a TIA to 2002 to 
move toward meeting ASCE 7, but 2007 is much better.

Most AHJ's will accept the new Standard if presented as an alternate.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message - 
From: Kurt Kingston [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Friday, January 18, 2008 10:10 AM
Subject: RE: Seismic Bracing and 2002 NFPA 13 Appendix


I'm re-posting this and any opinions or comments as to whether the
seismic bracing locations shown figures in the 2002 NFPA 13 Appendix are
OK to use would be appreciated.
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kurt
Kingston
Sent: Monday, December 17, 2007 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: Seismic Bracing and 2002 NFPA 13 Appendix

I would like to obtain your opinions as to whether the locations for the
seismic bracing in the 2002 NFPA 13 Appendix figures
A.9.3.5.6(a),(b),(c), and (d) are OK to use as shown if 2 and smaller
branch lines, and the structure is adequate to support the brace
spacing.
Thank you for your time,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Room Design

2007-12-21 Thread Jeff Hewitt

Bill,

Are they propped open with a fusible link???  You know, the 3-hr. wooden or 
rubber wedge fusible link??



Seriously, if these are light hazard spaces, the doors being open may not 
matter if you have minimum 8-in. lintels.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Friday, December 21, 2007 9:13 AM
Subject: Room Design



When you are performing an inspection of a system calculated using the
room design approach, how do you handle all of the doors that are
propped open?

Or, how do you calculate these systems?  Do you always go with the extra
two sprinklers and assume the doors will be held open?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: When is Earthquake Bracing Required?

2007-12-14 Thread Jeff Hewitt

This is a building code issue, not NFPA 13.

IBC 2003, Section 1621 Architectural, Mechanical, and Electrical Component 
Seismic Design Requirements, stipulates compliance with ASCE 7, 2002 
edition.


IBC 2006, Section1613 Earthquake Loads, stipulates compliance with ASCE 7, 
2005 edition.


You do NOT utilize the maps in NFPA 13, instead you utilize the prescribed 
method in ASCE 7, in conjunction with soil studies, seismic use group, 
seismic design category, spectral acceleration obtained from USGS maps, , 
etc...all used to arrive at a force factor which likely differs from the 0.5 
factor default value in NFPA 13.


Also, for mechanical piping, and NOT building structural importance factors, 
fire protection piping would be an importance factor of 1.5, regardless, 
because it is regarded as piping necessary for life safety.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Jimmy Waite [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Thursday, December 13, 2007 11:09 AM
Subject: When is Earthquake Bracing Required?


I have a question for the experts this morning.  Out here were are under 
the

IBC, and I believe that the Arch. and Structural Engineer have done their
jobs, but I still don't know if earthquake bracing is required. 
According

to the generic seismic zone maps available in NFPA, and according to
previous work that we've done in the area, we have NOT installed seismic
bracing before in this area.  BUT according to the structural engineer, 
this

is categorized as a design class C, use group III, and has an importance
factor of 1.25.  So, my question simply, is do we have to provide seismic
bracing when under these requirements?  The second, and more complicated
question, is where can I find (if there even is one) a chart, or a list, 
or

ANYTHING that will tell me when seismic bracing is required?  Which design
classes require bracing and which do not? Is the bracing requirement
dependent on the use group or vice versa?  I'd appreciate any guidance I 
can

get on this issue.  Thanks in advance.



Jimmy Waite

Burtell Fire Protection, Inc.

[EMAIL PROTECTED]

(406) 652-7697



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Design Area and Density

2007-12-12 Thread Jeff Hewitt
Ken,
   
  I am not in the office, and don't have my copy of my 13 handbook, but off the 
top of my head, so to speak, I disagree with Ed's last post.
   
  It is my understanding that the NFPA 13 verbage states words to the effect 
of...
  the 3000 sq.ft adjustment shall be applied AFTER all other adjustments have 
been applied.  Any suggestion of applying the QR reduction afterward is, in my 
opinion, incorrect.
   
  So, while I agree with any previous statement that you may slide along the 
appropriate occupancy class design curve to the appropriate lower density 
corresponding to 3000 sq.ft, it is not appropriate to apply additional 
corrections after the 3000 sq.ft. adjustment.
   
   
  Jeff Hewitt, PE, SET, SFPE (Professional Member)
  Corporate Engineer
  Bi-State Fire Protection Corporation
  636-946-0011
  636-946-5172
   

[EMAIL PROTECTED] [EMAIL PROTECTED] wrote:
  Ed,

So, if I understand you:

If I have an OH1 occupancy, and fall under the same criteria, say with a 
10'-0 ceiling, I could design:

a) With a minimum remote area of 3,000 square feet, using a density of 
0.12 gpm/sqft, based on the
area/density curve for OH1, and standard response sprinklers.

b) With a minimum remote area of 3,000 square feet, using a density of 
0.10 gpm/sqft, based on the
area/density curve for OH1, with the area being reduced by use of 
quick-response sprinklers without
revising the density, but not less than 3,000 square feet, as required 
by 11.2.3.1.4(3).

Is that about right?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com website



Ed Kramer wrote:
 Ken,

 Question #1: Yes

 Question #2: it depends. For light hazards, the answer is effectively 'no'.
 Section 11.2.3.2.7.2 says to apply the 3000 sf after all other
 modifications. Since the light hazard curve goes no higher than 3000 sf,
 the credit for QR sprinklers does you no good. On the other hand, the
 curves for the ordinary hazards go up to 4000 sf. So a designer could
 select an initial density/area of .15/4000 (ord group II), then apply a QR
 reduction, then increase the area back up to 3000 sf for a final
 density/area of .15/3000. But the final area must always be 3000 sf minimum.

 Ed Kramer
 Littleton, CO
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: 5 Gallon Bucket Storage

2007-12-06 Thread Jeff Hewitt

Steve,

I agree with 40-ft building height design, and exposed unexpanded Group A 
plastic,  but at that point there is no longer an advantage with K-25 due to 
the increased 12 head @ 50-psi design (due to the exposed plastics), and 
flow per head is approximately 178-gpm, for a total of at least 2136-gpm.


Instead, I would look at K-14 12 heads @ 75-psi, or K-17 12 heads @ 52-psi, 
which both only require approximately 121-gpm per head, or 1452-gpm total, 
to protect the very same exposed plastic, especially if you need a pump 
anyway.






Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Steve Leyton [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Thursday, December 06, 2007 11:15 AM
Subject: RE: 5 Gallon Bucket Storage


Sounds like exposed unexpanded, with a building height of 40'.   I think
the pitch is okay for ESFR, so try K25 at 50 PSI.   And bring your pump.

Steve Leyton
Protection Design  Consulting


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kevin
Pugh
Sent: Thursday, December 06, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: 5 Gallon Bucket Storage

Folks,

I am working on a facility that will be used to store 5 gallon buckets.
They will be stored on pallets. The pallets will be stacked 4 high,
making
a total storage height of 20'-0. There are no racks.
The eave height of the building is 28'-0, and the peak is approx. 38'
high,
the pitch is 1/2 on 12.
The buckets will be stored open end down.
The Production Manager at the plant couldn't tell me what type of
plastic
the buckets are composed of.
Do any of you have any advice as to what design criteria will be
required.
I have pretty good idea, but it's always good to have an outside
opinion.

Thanks for the help!!

Merry CHRISTmas!

Kevin R. Pugh
Sales / Project Manager
International Fire Protection, Inc.
5462 Able Court
Mobile, Al 36693
___

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: (no subject)

2007-11-13 Thread Jeff Hewitt

Joe,

try the FM data sheets.  There is a section on how to handle mezzanines and 
platforms in ESFR systems.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Joe Burtell [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Friday, November 09, 2007 10:28 AM
Subject: (no subject)



I have an ESFR system with an area of racks with a open grate mezzanine
floor. What would be the spacing of the intermediate level sprinkler below
the open grate?

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Carpet Rolls

2007-11-13 Thread Jeff Hewitt

Joe,

Try FM Data Sheet 8-30


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.
- Original Message - 
From: Joe Burtell [EMAIL PROTECTED]

To: sprinklerforum@firesprinkler.org
Sent: Tuesday, November 13, 2007 3:26 PM
Subject: Carpet Rolls



What standard or FM sheet covers solid pile of carpet rolls?

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: ESFR Draft Curtains

2007-11-01 Thread Jeff Hewitt

Look in the IFC

In IFC 2003,

910.3.4.1 Construction.  Draft curtains shall be constructed of sheet metal, 
lath and plaster, gypsum board, or other approved materials that provide 
equivalent performance to resist the passage of smoke,  Joints and 
connections shall be smoke tight.


910.3.4.2 Location and Depth.  The location and minimum depth of draft 
curtains shall be in accordance with Table 910.3.


I don't see any options there for draft curtains of 24-in. depth.  It looks 
like 48-in. to 72-in. depths depending on the Use Group and storage height.



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If you 
received this e-mail in error, please notify the sender immediately at the 
above captioned address.



- Original Message - 
From: Gregory Lindholm [EMAIL PROTECTED]

To: SprinklerFORUM SprinklerFORUM@firesprinkler.org
Sent: Thursday, November 01, 2007 4:08 PM
Subject: ESFR Draft Curtains


A GC is asking us what they should use for a draft curtain between the 
ESFR's and standard heads as specified in 2002, 8.4.6.4.1.


The project in question has the separation right along a 28 bar joist. What 
other guidelines can we give them other than noncombustible  24 ion depth? 
Does the draft curtain have to be sealed at the roof deck?


Greg Lindholm
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


  1   2   >