RE: 2'x4' Light Obstruction

2010-03-29 Thread Paul Pinigis
A 2' x 4' light fixture is only 2' wide, so there is no need for
protection beneath.  Although one dimension is 4', it is not 4' in its
least dimension (width).  Consider that there are probably conduits,
pipes, and even the grid for the ceiling that are over 4' long, but you
do not sprinkler below them for the same reason (the are under 4' wide).

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Medina Jr
Sent: Monday, March 29, 2010 3:13 PM
To: SprinklerFORUM@firesprinkler.org
Subject: 2'x4' Light Obstruction

I have a situation where I have an open ceiling tiled hallway and there
are 2' x 4' light fixtures. According to NFPA-13 (2007) Sec. 8.6.5.3.3
it seems I need Coverage under a 4' wide fixed obstruction. My
sprinklers are 5' above the lights. Do they need to have ceiling tiles
in place around it or is there a solution I am missing. Any help would
be greatly appreciated.


George Medina Jr. 
323-236-1640
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Accidental Fusing

2010-02-05 Thread Paul Pinigis
Brad,
 
Are you a lawyer?
 
Paul



From: sprinklerforum-boun...@firesprinkler.org on behalf of Brad
Sent: Fri 2/5/2010 1:02 PM
To: sprinklerforum@firesprinkler.org
Subject: Accidental Fusing



Do any contractors have experience with heads fusing 'accidentally'?

Did a lawsuit result?

I would appreciate your thoughts on this specific scenario:



-Attic Dry System in service, 33 PSI air

-early July-- Kansas

-1 head out of many fused (at ridge)

-1/2, 212F, Standard Response, Reliable Link Type

-Soffit vents around perimeter (ventilated)

-no mechanical damage to head

-fused parts (at least the link) was not found in debris



Thank you very much,

Brad

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: standpipe for attic?

2009-11-11 Thread Paul Pinigis
Per section 1509.2 of the 2006 IBC, a penthouse or rooftop enclosure can
be up to 1/3 of the area of the roof.  Over that and it is a floor.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Wednesday, November 11, 2009 3:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: standpipe for attic?

Same sort of question could be asked of a Mechanical penthouse How big
does it have to be before it's a floor, and not just a box set on the
roof?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill
Brooks
Sent: Wednesday, November 11, 2009 11:49 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: standpipe for attic?

Normally an attic is not considered a story, but it could be.  If it is
not
a story and if there is no stair access to the space, there may not be a
need to provide a standpipe connection for this area.  However, IBC
Section
1209.3 does provide for access to concealed spaces such as attics.  My
assumption would be that a standpipe connection from the floor below
would
be the source of protection for the attic above if access openings are
provided.  IBC 905.4, subpar 6 would be the trigger to install
additional
outlets on the floor below if the access openings are not sufficient.

Perhaps John Drucker could add the correct interpretation if I have led
in
the wrong direction.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd
Williams
Sent: Wednesday, November 11, 2009 12:11 PM
To: sprinklerforum@firesprinkler.org
Subject: standpipe for attic?

I am working on a building where part of the 3rd floor is occupied
(center
core) and the rest (wings and area over core) is unoccupied attic. The
building is fully sprinklered, including the attic. Does the standpipe
coverage have to reach the remote part of the attic spaces or just the
occupied part? Couldn't find anything in 14.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Chance to Make a Difference in Military Standards

2009-10-09 Thread Paul Pinigis
Bill,

What section prohibits the placement of risers on exterior walls?

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill
Brooks
Sent: Friday, October 09, 2009 10:10 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Chance to Make a Difference in Military Standards

I'd suggest a review of the ATFP requirements and the prohibition of
riser
placement next to an exterior wall.  When is it permitted to place a
riser
adjacent to an exterior wall, and what type wall construction would
permit
this?  Does adequate standoff distance provide an exception to this
requirement?  Does this mean a standpipe riser cannot be placed in a
stairwell since a stairwell always has an exterior wall?  If the
exterior
wall is not suitable construction, how far inside the building must the
riser be located?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Kowkabany
Sent: Thursday, October 08, 2009 10:57 AM
To: sprinklerforum@firesprinkler.org
Subject: Chance to Make a Difference in Military Standards

Guys and Gals, 

 

After our discussion on this forum a couple weeks ago, our local SFPE
chapter is setting up a symposium to discuss the military design
standards
and how they can be improved.  There will be ranking military
representation
at this meeting and Navy FPE's who really care about the process and
improving it.  We are also bringing our local FPE's who do a  large
volume
of military work and some excellent local contractors to this meeting,
which
will take place two weeks from today.

 

My question to you is - how do you think the UFC codes, ETL's, and other
military design standards be improved specifically?  What types of
things
could be added or deleted to add more value to our governmental
projects,
reduce wasteful spending, and maintain or improve the level of fire
protection in these facilities.

 

Here are some things I intend to table for starters:

 

1)  3,000 sqft design area - reduce this to commercial or FM
standards
to save money.  There is no data I am aware of that shows that doubling
the
remote areas in NFPA 13 provide better fire protection.

2)  12 psi mandatory backflow preventer pressure drop regardless of
type
- why force this when most installations are double-checks and this can
often result in the need for a fire pump which in turn, is less reliable
of
a system and more expensive.  

3)  Doubled hose allowances - What data backs up this requirement
and
why not go with what works for the commercial world, FD operations on
base
seem similar to civilian operations and requirements for most buildings.

 

Any thoughts you may have would be greatly appreciated and would love
some
input from this highly knowledgeable group.  Plus you will be doing a
service for your country and there is a good chance that some positive
change will come of this.  We intend to write a position paper based on
the
results and to collaborate closely with the military.

 

Thank you very much in advance,

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

60 Ocean Boulevard, Suite 15

Atlantic Beach, FL 32233

904-652-4200 Phone

904-212-0868 Fax 

 

We have moved.  Please note our new address.

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Virginia Zero Sq. Ft. policy? yes or no

2009-07-31 Thread Paul Pinigis
Virginia adopts the IBC with some amendments, but there is no zero sq.
ft. policy.  

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, July 30, 2009 11:22 AM
To: sprinklerforum@firesprinkler.org
Subject: Virginia Zero Sq. Ft. policy? yes or no

Can anyone from Virginia tell me if the State has a zero sq. ft policy
for sprinklers?  We have a large F-2 mfg. area which doesn't require
sprinklers based on the IBC.  Building is around 200 ft in height in
places, single story with working mezzanines inside with some misc.
office spaces located throughout.
 
Trying to make sure there are no surprises.  
 
Thanks,
 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Hydrant Flow test results

2009-06-23 Thread Paul Pinigis
Any single-hydrant test is questionable to begin with, but if two tests
are done they should yield identical graphs.  Pitot pressures of less
than 10 psi are generally unacceptable.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 3:25 PM
To: sprinklerforum
Subject: Hydrant Flow test results

Have a question regarding hydrant flow tests.

We have received a report where the contractor flow a single 2 1/2
outlet
and gave us static, residual, pitot and calculated flow.  He then
performed
another test using the 4 1/2 outlet on the hydrant, again giving us
values.

Plotting the graph, is there supposed to be a correlation between the
testing of the 2 1/2 versus the 4 1/2 or are they supposed to be used
separately.  For example, when graphing the 2 1/2 outlet, the 4 1/2
outlet
info should be hitting this line or not??

Also, is a pitot reading of a range of 4 to say 8 on a 4 1/2 outlet
valid
data?

We're not sure how to use this info.

Richard
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: UAE, Saudi, Codes and standards and component certifications

2009-05-11 Thread Paul Pinigis
We often hire a local architect to assist in code evaluations to ensure
local-code compliance.  I do have the fire code of Taiwan if anyone
speaks Mandarin.  

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
bill.bro...@brooksfpe.com
Sent: Monday, May 11, 2009 3:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: UAE, Saudi, Codes and standards and component
certifications

Do not assume any U.S. standards are the most stringent.  I have seen
authorities ask for 1) sprinklers in concealed spaces because of minor
amounts of combustibles, 2) clean agent systems in electronic areas just
because there is an NFPA standard for these systems, 3) standpipes in
single story buildings because there is an NFPA standard, 4) smoke
detection systems above and below ceilings in fully sprinklered
buildings, 5) prohibit a sprinkler head from being placed on anything
other than a branch line (a previous discussion we had - the forum
response was generally that's nuts, why would anyone misinterpret NFPA
13 that way).

If possible, it is good policy to separate yourself from any compliance
with host country codes and standards.  If you are a sub to a sub to a
sub, like most of us are, see that the guy at the top of the food chain
hires a host country entity to determine your scope and the standards
you will follow, including the local interpretations.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

 Original Message 
Subject: UAE, Saudi, Codes and standards and component certifications
From: craig.pr...@ch2m.com
Date: Mon, May 11, 2009 12:05 pm
To: sprinklerforum@firesprinkler.org

I know we have a few international participants here and I need to know
if someone can assist in telling me what Codes are used for fire
protection in the above mentioned areas. Also, we use Underwriters
Laboratories (U.L.) here as our testing agency which NFPA indirectly
references and I'm wondering what is the equivalent over there.




Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Branch line insulation

2009-04-24 Thread Paul Pinigis
Insulation on a pipe with non-flowing water is pointless (except for
temporary exposures to low temperatures).  Insulation can only slow the
transmission of heat from the pipe, it does nothing to produce heat.  

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell
Sent: Thursday, April 23, 2009 3:34 PM
To: AFSA
Subject: Branch line insulation

NFPA13 2007. Is 8.16.4.1.2 telling me that (steel) branch lines cannot
be
insulated (insulation only)? Also is it telling me that only small areas
can
be heat traced?

We have always used dry or anti-freeze systems so I'm not up to date on
this.

 

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

russ...@brownautomatic.com

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Walk-in cooler

2009-04-23 Thread Paul Pinigis
What you have described is a room, and just like every other room in a
sprinkered building it must also be sprinklered.  That fact that it is
cold in there is irrelevant.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Thursday, April 23, 2009 12:14 PM
To: sprinklerforum@firesprinkler.org
Subject: Walk-in cooler

Generally the industry practice (from what I know) is to provide
sprinklers
in walk-in coolers and freezers. The cooler I am looking at is a beer
cooler
approx. 30 feet long, 10 feet deep and 7 feet high. It is full with
shelves,
and no one could walk-in. Would it have to be sprinklered? Anyone has
come
across a similar situation or have any opinions?

Tony 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
It depends upon the distance between buildings and the percent of open
wall space under the roof.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 9:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Possible IBC question

I am looking for some code help. According to NFPA 13 8.2.4 you can have
separate buildings that share a common roof, walls or passageway be
protected by one riser. Does anyone know if the IBC contradicts this? I
have
an architect telling me I have to have a separate riser for each section
of
building. They claim that I can have the risers in the same room but
that
each building section must have a separate riser.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
If they are actually separated by fire walls, and not just fire-rated
walls, then they are separate buildings per the IBC.  But, yes, you can
use one riser to feed both buildings provided that you protect the
connecting pipe from freezing temperatures and you do not exceed the
maximum allowable area for the system.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 10:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Possible IBC question

The buildings are actually just additions to an existing building and
they
are separated by two adjacent fire walls.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Paul
Pinigis
Sent: Monday, March 23, 2009 10:03 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Possible IBC question

It depends upon the distance between buildings and the percent of open
wall space under the roof.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 9:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Possible IBC question

I am looking for some code help. According to NFPA 13 8.2.4 you can have
separate buildings that share a common roof, walls or passageway be
protected by one riser. Does anyone know if the IBC contradicts this? I
have
an architect telling me I have to have a separate riser for each section
of
building. They claim that I can have the risers in the same room but
that
each building section must have a separate riser.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
One last thing to keep in mind is that some water companies demand
separate services if they are considered separate buildings; that
supersedes the requirements of NFPA 13.   

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Monday, March 23, 2009 12:04 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Possible IBC question

I would add to everyone else's replies that it is NOT the intent of NFPA
13 to require separate systems in this situation, whether or not the
structure is considered to be divided into separate buildings, or just
separate fire areas or occupancies - see 8.2.4, 2007 ed.

And thanks again to whoever turned me onto that - saved us a lot of
bitchin' and pissin' with the AHJ on that particular project.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 6:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Possible IBC question

I am looking for some code help. According to NFPA 13 8.2.4 you can have
separate buildings that share a common roof, walls or passageway be
protected by one riser. Does anyone know if the IBC contradicts this? I
have
an architect telling me I have to have a separate riser for each section
of
building. They claim that I can have the risers in the same room but
that
each building section must have a separate riser.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3954 (20090323) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3954 (20090323) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Labeling

2009-03-05 Thread Paul Pinigis
On F-Troop, FIRE WATER was a beverage.  :)

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer
Sent: Thursday, March 05, 2009 1:54 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Labeling

That's how I read it also.  If your arch buddy wants flow arrows, pipe
ID
markers (FIRE WATER- DO NOT DRINK), that's not required by 13.  So if
he/she
wants them, it should be a change order.

Ed Kramer
Littleton, CO

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, March 05, 2009 11:38 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Labeling
 
 I read that to mean the identification label put on by the
manufacturer
 
 not the flashy little flow stickers  such?
 
 
 Brian Harris
 FDFP INC.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed
Kramer
 Sent: Thursday, March 05, 2009 1:30 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Labeling
 
 Check out section 6.3.8, though the architect's definition of
'Labeled'
 may
 mean something different.
 
 Ed Kramer
 Littleton, CO
 
 
  Forum,
  I just wanted to double check myself before I put my foot in my
mouth,
  I'm working on a school and the spec says that pipe is to be labeled
  per
  NFPA-13 (2002). I don't remember seeing anything in NFPA that talks
  about labeling pipe, I just did another quick search and didn't come
  up with anything. Does anybody know if labeling is talked about in
 there?
  If it is and my understanding is correct NFPA-13 would only tell you
  how to do it and not when to do it, correct?
 
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to:
 techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email to:Sprinklerforum-
 requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to:
 techsupp...@firesprinkler.org
 
 To Unsubscribe, send an email to:Sprinklerforum-
 requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PE Peer Review

2009-02-26 Thread Paul Pinigis
The reduction in design area has nothing to do with the likelihood of a
fire, it is related to the ability of the sprinkler system to control
the fireperiod.  This is a great example of the reviewer suffering
rectal cranial inversion.

I will bet that in typical RJA fashion the review was littered with
statements-of-the-obvious that have nothing to do with deficiencies in
your design like: comply with NFPA 13, follow the obstruction rules,
take an umbrella if its raining... and all of the other fluff and filler
they use to make their reviews appear extensive.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Wednesday, February 25, 2009 6:03 PM
To: sprinklerforum@firesprinkler.org
Subject: PE Peer Review

I would like the take from the PE's on forum on how to deal with a plan
review comment from an unnamed engineering firm (RJA).

Due to the higher than normal potential for a fire in the occupant
sleeping and common areas, the reduction in fire are (remote area) for
quick response sprinkler in accordance with NFPA #13 Figure 11.2.3.2.3.1
is not a good engineering practice. Please revise the hydraulic
calculation to account for at least the minimum 1500 square foot design
area as specified by NFPA #13.

The hazard is a dormitory at a minimum security prison.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: underground pre-action piping

2009-02-20 Thread Paul Pinigis
I would suggest mechanical-joint cement-lined ductile iron, but I do not
know how you are going to drain it short of putting in a pit. 

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Lori
Kitchen
Sent: Friday, February 20, 2009 10:14 AM
To: sprinklerforum@firesprinkler.org
Subject: underground pre-action piping

We are working on the underground for a project where a remote building
is
to be protected by a pre-action system whose valve is in a different
building 50ft away.  The underground connecting these two buildings is
to be
part of the pre-action system (piping filled with air).  In other words,
the
pre-action valve is in building A.  The piping runs underground (after
the
valve) to building B.

This is a new one for us.  My questions are what type of pipe do you use
for
this purpose and how do we drain the water out of the underground?

I appreciate any info!

 

 

Lori Kitchen

Whitewater Fire Sprinkler

 

316-295-4120 (office)

316-295-4162 (fax)

 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: * Possible Spam *Re: Bedbug Treatment

2009-02-06 Thread Paul Pinigis
I agree that it would be a waste to simply dispose of perfectly good
sprinklers, and I personally would have no problem with someone reusing
them for such an application.  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thomas
Watt
Sent: Friday, February 06, 2009 1:05 PM
To: sprinklerforum@firesprinkler.org
Subject: * Possible Spam *Re: Bedbug Treatment

I know what the code says but it seems wasteful to use these heads for
24 
hours and then throw them away. I got the feeling that the profit margin
on 
this job was pretty slim already.
As far as firewatches go, having to rely on hotel staff for this does
not 
make me feel confident at all. Especially when the management wants this
all 
done quickly and quietly.(hush-hush)


- Original Message - 
From: Paul Pinigis p.pini...@haengineers.com
To: sprinklerforum@firesprinkler.org
Sent: Friday, February 06, 2009 11:40 AM
Subject: RE: * Possible Spam *Bedbug Treatment


Installing intermediate temperature sprinklers seems like the most
sensible approach, but you could not reinstall them elsewhere because
they are now used.

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thomas
Watt
Sent: Friday, February 06, 2009 8:21 AM
To: sprinklerforum@firesprinkler.org
Subject: * Possible Spam *Bedbug Treatment

Hello group,

Several months ago I was sent to remove the (12)sprinklers from a hotel
room so that it could be heat treated for a bedbug infestation. This
process involves heating the room to over 130 degrees. My instructions
were to remove the sprinklers and replace with nipple/caps until the
next day when the sprinklers could be replaced.

I know in many cases the heating equipment is truck mounted and the
heating ducts are stretched into the unit to be treated. In this case,
the heater/blowers were all portable units. In retrospect, with all of
these appliances in this unprotected space in an occupied wing of this
hotel, this was a catastrophe waiting to happen.

1) Could I have replaced the 155* heads with intermediate temp heads?
2) Could I reuse these heads for the next bedbug job?

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)







Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com
Version: 8.0.233 / Virus Database: 270.10.16/1930 - Release Date:
2/2/2009 
7:51 AM

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Sprinklered vs Sprinkled

2009-01-15 Thread Paul Pinigis
Yes, I have heard it many times here in Virginia, and always find it amusing. 

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
bill.bro...@brooksfpe.com
Sent: Wednesday, January 14, 2009 11:47 PM
To: sprinklerforum@firesprinkler.org
Subject: Sprinklered vs Sprinkled

Actually this is a serious question.

Is there anywhere in the country where the term sprinkled is commonly
used by sprinkler industry types to describe a building with a sprinkler
system?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

RE: another fire - this will be interesting

2009-01-07 Thread Paul Pinigis
The lack of detail on the engineer's sprinkler drawings is often
dictated by the client, not the A/E firm.  For example, the Navy will
not allow us to do detailed designs because they (like many others)
believe that will lead to change orders.  Somehow they don't have a
problem with the HVAC engineer or the plumbing engineer showing their
detailed designs.  I would like to see equal treatment; the HVAC
engineers should show a hatch pattern on the floor plan with a note that
says deign ductwork to provide a comfortable environment.. 

Paul Pinigis, P.E.
Life Safety Department Head



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, January 07, 2009 10:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

You'll have to do more than just make your magical FPE's appear from the
sky, you'll have to change the mindset of an entire industry. 

For too long the A/E industry has felt it was a waste of time and money
to do detailed design for fire protection, the thought being that since
the contractor did all that for free, why duplicate the effort.  Less
hours spent on fire protection meant more hours to be used by someone
else or could be saved altogether.  That makes the PM look good, hours
unspent=bigger bonus.

So even if you did have your super FPE's appear, they would still not be
able to produce the documents the contractors would love to see.

Trying to educate project managers, schedulers, department managers
etc.. is an uphill battle.  They don't understand the FP industry,
how it works, who does what, submittals to AHJ's, minimum information
required on a drawing package, when in the course of the project fire
protection needs to start and finish, what info is needed to do the fp
design work (when you are doing more than an X on a drawing, and the
list of obstacles goes on and on.  Next project, you start the battle
all over again.

Other disciplines don't understand the rules you have for head spacing,
deflector distances below decks, obstructions, water pressure and flow
issues, etc. Most think FP as being able to move where ever so they have
more room and are often told that very thing by their supervisors.

You don't know how many times I've been told by ME's who are supposed to
be responsible for FP work that it is so confusing.  What's scary is
most probably know just enough to pass the FPE.  So that's obviously not
the answer to the overall problem.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Tuesday, January 06, 2009 11:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

We'd need several hundred qualified FPEs (or equal) to fall out of the
sky in order to do what you  say, as desirable a concept as you present.
That and a couple thousand more so we contractors can put them on staff
so we can evaluate water supplies and perform hydraulic calculations in
accordance with the SFPE White Paper (unless the more recent revs have
allowed us to calc systems like we've been doing as an industry since
there were calcs).

Instead we have FPE-Plumbing Designer ACTING like FPEs despite being
only casually familiar with our industry, codes, standards, materials,
etc.- i.e., practicing outside their area of competence. 

And so we don't just call this PE bashing, I'll point out that
contractors evaluating water supplies- and that would be all of us
performing calcs based on some flow test, ours or someone elses- need to
be aware of lowest tank gradient, the importance of correcting for
elevation and other corrections needed to move the data correctly from
the test to the floor flange. I have a project where my competitor doing
an adjacent building on same site off same main is using a flow test
result that is 10 PSI higher than mine, with twice the flow. I've become
familiar with the site, water supply, and did a more accurate test than
they did, I guess that's the price of being able to sleep at night.

glc

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Paul
Pinigis
Sent: Tuesday, January 06, 2009 10:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

Very well said John.  This is exactly the approach that we take; we look
at the building or project holistically and our fire protection
engineers direct the architect, mechanical, electrical, structural,
telecom, etc. to ensure coordination and compliance

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
Very well said John.  This is exactly the approach that we take; we look
at the building or project holistically and our fire protection
engineers direct the architect, mechanical, electrical, structural,
telecom, etc. to ensure coordination and compliance.  

Paul Pinigis, P.E.
Life Safety Department Head

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520 
d:(804) 521-7011

http://www.haengineers.com
 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker
Sent: Tuesday, January 06, 2009 9:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting


Simply put fire protection is not seamless. Often enough it's a
patchwork of pieces and parts assembled without a clear and common
objective. We see this everyday with smoke detectors being installed in
unsprinklered elevator hoistways because no one told the alarm engineer
that sprinklers had been eliminated by the sprinkler engineer, or fire
dampers installed in one hour walls in fully sprinklered buildings
because no one told the mechanical engineer. The disconnect with the
fire service is yet another example, site planning left to the civil
engineer without regard to fire protection needs.

What we need are MEPF firms, engineering firms that employ and fully
utilize fire protection engineers to look at the big picture, assess,
plan, design, coordinate and supervise cost effective and efficient fire
protection solutions. 

If as a fire protection engineer you're simply designing fire alarm or
sprinkler systems you are not working to your full potential !  There
are firms that provide life safety analysis to provide passive fire
protection solutions, often coined working for the dark side they
nonetheless do what others are not, looking at the big picture. High
rise sprinklers in Chicago or San Diego anyone ? 

So how does the active fire protection community counter this claim,
perhaps by long term planning, synergistic value driven engineering. It
goes all the way back to codes and standards, how many cycles did it
take to recognize sprinklers in fully sprinklered buildings for
notification survivability on fire alarm systems ?

One stop shopping ladies and gentlemen, one stop shopping.

Sincerely

John Drucker
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, January 05, 2009 10:36 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

Ron said (I suspect the savings in mains, hydrants, fire stations,
apparatus and firefighters is way more than a wash in fully sprinklered,
planned communities than the cost of sprinklering schools).

Were these savings realized?  Last I read which was a long time ago
there was very little saved on the reduction in the list you provided.
They never actually followed through in reducing mains and limiting
stations etc.  I will certainly say in the macro scale these saving are
not being fully realized.  Hell we still have fully paid stations in
many departments that average  1 call a day and plenty more that are 
2.  As a pay-per-call volunteer I saw more fire than many paid guys in
these parts.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron
Greenman
Sent: Friday, January 02, 2009 2:05 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: another fire - this will be interesting

Good point so far overlooked. There's also the dubious saved
foundation success that may have not been worth the risk of going into
harm's way. And no one has brought up the environmental advantages of
sprinklers--less smoke, less destroyed building materials to dispose of,
less dirty water to process and, of course, less water used overall. And
the Scottsdale less public money spent on firefighting infrastructure (I
suspect the savings in mains, hydrants, fire stations, apparatus and
firefighters is way more than a wash in fully sprinklered, planned
communities than the cost of sprinklering schools).

On Fri, Jan 2, 2009 at 11:49 AM, Dave nomore...@yahoo.com wrote:
 Since we are offering up various thoughts and theories on the general
application of sprinklers .  Regardless of how much egress time is
allegedly available or occupant ability to respond or even construction
materials  methods - there still is a fire in a building -  Presuming
we get

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
We have 5 registered FPEs (not turd-herders pretending to be FPEs) and 5
EITs who will get registered as they become eligible.  Most of our
design work is done by our designers (two Level IV, and one Level II).
Our engineers are responsible for the ENGINEERING activities.

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Tuesday, January 06, 2009 11:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

We'd need several hundred qualified FPEs (or equal) to fall out of the
sky
in order to do what you  say, as desirable a concept as you present.
That
and a couple thousand more so we contractors can put them on staff so we
can
evaluate water supplies and perform hydraulic calculations in accordance
with the SFPE White Paper (unless the more recent revs have allowed us
to
calc systems like we've been doing as an industry since there were
calcs).

Instead we have FPE-Plumbing Designer ACTING like FPEs despite being
only
casually familiar with our industry, codes, standards, materials, etc.-
i.e., practicing outside their area of competence. 

And so we don't just call this PE bashing, I'll point out that
contractors
evaluating water supplies- and that would be all of us performing calcs
based on some flow test, ours or someone elses- need to be aware of
lowest
tank gradient, the importance of correcting for elevation and other
corrections needed to move the data correctly from the test to the floor
flange. I have a project where my competitor doing an adjacent building
on
same site off same main is using a flow test result that is 10 PSI
higher
than mine, with twice the flow. I've become familiar with the site,
water
supply, and did a more accurate test than they did, I guess that's the
price
of being able to sleep at night.

glc

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Paul
Pinigis
Sent: Tuesday, January 06, 2009 10:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

Very well said John.  This is exactly the approach that we take; we look
at the building or project holistically and our fire protection
engineers direct the architect, mechanical, electrical, structural,
telecom, etc. to ensure coordination and compliance.  

Paul Pinigis, P.E.
Life Safety Department Head

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520 
d:(804) 521-7011

http://www.haengineers.com
 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker
Sent: Tuesday, January 06, 2009 9:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting


Simply put fire protection is not seamless. Often enough it's a
patchwork of pieces and parts assembled without a clear and common
objective. We see this everyday with smoke detectors being installed in
unsprinklered elevator hoistways because no one told the alarm engineer
that sprinklers had been eliminated by the sprinkler engineer, or fire
dampers installed in one hour walls in fully sprinklered buildings
because no one told the mechanical engineer. The disconnect with the
fire service is yet another example, site planning left to the civil
engineer without regard to fire protection needs.

What we need are MEPF firms, engineering firms that employ and fully
utilize fire protection engineers to look at the big picture, assess,
plan, design, coordinate and supervise cost effective and efficient fire
protection solutions. 

If as a fire protection engineer you're simply designing fire alarm or
sprinkler systems you are not working to your full potential !  There
are firms that provide life safety analysis to provide passive fire
protection solutions, often coined working for the dark side they
nonetheless do what others are not, looking at the big picture. High
rise sprinklers in Chicago or San Diego anyone ? 

So how does the active fire protection community counter this claim,
perhaps by long term planning, synergistic value driven engineering. It
goes all the way back to codes and standards, how many cycles did it
take to recognize sprinklers in fully sprinklered buildings for
notification survivability on fire alarm systems ?

One stop shopping ladies and gentlemen, one stop shopping.

Sincerely

John Drucker
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, January 05, 2009 10:36 AM
To: sprinklerforum@firesprinkler.org
Subject: RE

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
There is your problem!  You have electrical doing fire alarm and
mechanical doing sprinkler!!!  You just defined the need for a qualified
FPE to perform those functions (and many more).  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Tuesday, January 06, 2009 11:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

Unfortunately, even just MPE firms can't co-ordinate within the firm,
adding
another layer (F) won't improve the end product. The E showed the smoke
detector, the M said sprinkler per code, and the P never even remembered
the
sump in the elevator pit. Add an (F) to that and I can assure you that
it
will be all F'ed up!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John
Drucker

What we need are MEPF firms, engineering firms that employ and fully
utilize
fire protection engineers to look at the big picture, assess, plan,
design,
coordinate and supervise cost effective and efficient fire protection
solutions. 


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
Our firm will not allow anyone to work outside of their area of
expertise, but some firms do.  I received a call from a mechanical
engineer a few years ago who was in desperate need of help; his boss
appointed him as the company's FPE and he had no experience in any
aspect of fire protection engineering (his previous responsibility was
designing industrial valves).  

Paul Pinigis, P.E.
Life Safety Department Head




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Tuesday, January 06, 2009 3:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

Actually this is the engineering community's problem, not mine. You're
the
one's that allow incompetent work to be done by engineers that are
neither
qualified or trained to do it. Working Outside their area of expertise
If
all states licensed engineers by discipline or degree, or had some
really
effective bylaws and penalties for engineers that do work outside their
knowledge or training it might help. Most states like Colorado allow the
engineers to Self Police their brother engineers, and unless someone
dies
or a huge financial loss occurs, they rarely do more than send censure
notes to fellow engineers.(Please don't be bad anymore, and take that 3
day
NFPA 13 class, cause that's all the training you need to DESIGN fire
sprinkler systems, because you already know everything else.)

Just as there are good and bad contractors, there are good and bad
engineers. To the good ones I apologize.
To the good ones I say help your selves, do something about all the bad
ones!
For the good and bad contractors? Licensing doesn't work. But educating
your
AHj's can help ensure that shoddy work doesn't take place where you
work.
Raise the bar for everyone, don't stoop to the level of the competition.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Paul
Pinigis
Sent: Tuesday, January 06, 2009 12:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: another fire - this will be interesting

There is your problem!  You have electrical doing fire alarm and
mechanical
doing sprinkler!!!  You just defined the need for a qualified FPE to
perform
those functions (and many more).  

Paul Pinigis, P.E.
Life Safety Department Head





___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Residential Sprinkler Ordinances

2008-08-15 Thread Paul Pinigis
It appears that all jurisdictions that adopt NFPA 101 have, either 
intentionally or inadvertently, adopted the requirement for sprinkler 
protection in all one- and two-family homes.  The only state that comes to mind 
as having adopted NFPA 101 is West Virginia; and I do not know if they are 
actually enforcing that provision of the code. 

Paul J. Pinigis, P.E.

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John T. Johnson, 
CFPS
Sent: Friday, August 15, 2008 1:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Residential Sprinkler Ordinances

Good Afternoon,
 
A friend is partnering with an editor for a series of articles about 
residential sprinklers in a newspaper in regards to the upcoming vote at the 
IRC meeting in Sept. She was asking for names of cities, municipalities, and 
townships that have adopted residential sprinkler ordinances in the last 2-3 
years throughout the U.S. I imagine the forum would know of a few...
 
Thanks, 

John T. Johnson, CFPS
Technical Trainer/Firefighting Instructor
--
Fire Sprinklers/Smoke Detectors Save Lives*



  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: NFPA 101 Dwelling Unit Sprinklers

2008-08-12 Thread Paul Pinigis
That is really funny!  I read it the same way.  If you provide party
walls between the townhouses they become single family homes and require
sprinkler protection, but if you don't they are garden apartments and do
not require sprinklers.  I would be very interested to know the logic
behind this also.  I would also be interested to know if state that
adopt NFPA 101 are enforcing the requirement for sprinklers in single
family homes.

Paul J. Pinigis, P.E.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, August 12, 2008 8:37 AM
To: sprinklerforum@firesprinkler.org
Subject: NFPA 101 Dwelling Unit Sprinklers

I have a quick question on sprinkler requirements for Dwellings as
defined 
in NFPA 101 2006 edition.

We are working on a 600+ unit residential community overseas that
includes 
single family, two family, quadraplexes and apartments.  NFPA 101,
section 
24.3.51 (one and two family dwellings) indicates that all new one- and 
two-family dwellings shall be protected throughout by an approved 
automatic sprinkler system in accordance with 24.3.5.2.  I read this to

say that all new single and two family units will need to be provided
with 
sprinklers under this code, and I do not see any exceptions in 24.3.5.2

NFPA 101, section 30.3.5.1 (new apartment buildings) states that All 
buildings, other than those complying  with 30.3.5.2 shall be protected 
throughout by an approved, supervised automatic sprinkler system . . . 
Section  30.3.5.2 (1) provides an exception that sprinkler systems are
not 
required in buildings where every dwelling unit provides an exit door 
opening directly to the street or yard at ground level.  The quad units

are 4 side by side town houses with exits at ground directly outside to
a 
yard and street. 

Based on the sections noted above, I think I am required to sprinkler
the 
one and two family units but not the quads.  In addition, if the
architect 
provides a rated separation between the quads that is approved by the
AHJ, 
I can call each unit a one family swelling and use chapter 24, but that 
would then require sprinklers.  I am struggling with the logic of this.
In 
addition, if I am understanding this correctly, I could present a site 
plan to the AHJ that sprinklers the one and two family swellings, the 42

unit apartment buildings, but not the quad unit town houses and be code 
compliant, albeit in my mind a little bit silly.  This does not sit
right 
with me.

What am I missing, or is this just one of those things?

I feel like Monday never ended.

Thanks.

Andrew Weisfield



This email is intended for named recipients only.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Shelf Storage

2008-08-12 Thread Paul Pinigis
Keeping it brief Bill?  

Paul Pinigis
Hankins and Anderson

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Tuesday, August 12, 2008 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: Shelf Storage


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

RE: Soleniod valve

2008-08-11 Thread Paul Pinigis
I don't think that you will find a solenoid valve that is listed as
preaction valve, but the engineer of record should be able to point you
to one if it exists and was the basis of his design.  Preaction valves
do have solenoid valves in them, but the solenoid is not usually listed
for the purpose you describe.  

I will bet you that the engineer of record is turd herder, not an FPE.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Keith
Pepin
Sent: Monday, August 11, 2008 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: Soleniod valve

The engineer of record for a project has provided me with a drawing to
provide sprinklers in an IT room. His proposal is to install a solenoid
valve on the wet sprinkler line that is wired closed so that the line
can be
drained of water, in essence, making that portion dry. He indicated that
the
solenoid will be wired to a smoke/heat detector that will open in the
event
of a fire, charging the line. The sprinkler head will remain closed
until
they reach the operating temperature. 

The engineer does not want water in this room until needed. What do you
think about his school of thought? At the very least, the valve would
have
to be approved for fire sprinkler use?

 

Thanks

Keith

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Floating Ceilings

2008-08-05 Thread Paul Pinigis
Rick, 

I agree with you, you no longer have a noncombustible concealed space
above the ceiling.  When we see architects attempt this at the design
stage we usually steer them away from the cloud ceiling; when we cannot,
we sprinkler above and below the ceiling (obstruction).  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rick
Green
Sent: Tuesday, August 05, 2008 8:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Floating Ceilings


I am in the design phase installing wet pipe sprinkler systems
protecting new schools.

I have noticed that in several of the rooms in the schools(cafeteria,
band room, main corridor that runs the length of the school), architect
has designed lay-in ceiling systems with gaps ranging from 4 to 12
along the walls and between sections of ceiling within the rooms
(floating ceiling sections).

I do not believe my non-combustible concealed space above the ceilings
is concealed anymore and may require protection.

Has anyone dealt with this?

I have heard some discussion that if the total square feet of the
openings is below a certain percent of the total square foot of a space,
sprinkler protection above the space may not be required?

Interesting thing is that the school is being built as a Green project
and seems like the designed openings would make the schools less energy
efficient.

Anyone's help would be most appreciated...



Rick E. Green
District Manager
East Coast Fire Protection, Inc.
1113 Cavalier Boulevard
Chesapeake, Virginia 23323
757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell)
[EMAIL PROTECTED]

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Stair shafts

2008-07-31 Thread Paul Pinigis
Most carpeting meets the definition of non-combustible, but I would
suggest checking the manufacturers cut sheet to verify.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Margaret
Zabel
Sent: Thursday, July 31, 2008 11:39 AM
To: Sprinkler Forum
Subject: Stair shafts

Using NFPA 13-2002, paragraph 8.14.3.2 describes the
requirements for sprinklers in non-combustible stair
shafts.

Would a non-combustible construction stair shaft
(concrete stairs, sheetrock/rated walls) that has
carpet on the landings and stair treads be considered
non-combustible?  Assuming the stairs are over 4'-0
wide, should there be sprinklers located throughout
the shaft -- below treads and stairs?

Thank you,

Margaret Zabel
Cisco Fire Sprinklers
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Water Supply

2008-07-30 Thread Paul Pinigis
I would suggest redoing the flow test and using a playpipe for better
accuracy. If the first test was done with an open hydrant butt and a
factor or 0.9, you may find that the estimate was too conservative.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Wednesday, July 30, 2008 11:58 AM
To: SprinklerFORUM
Subject: Water Supply

I have a project where the system demand with hose allowance exceeds the
city supply by 31 GPM. It's still under the curve but the city flow test
was
1210 and my system demand is 1241. Is there anything in the codes that
allows me to exceed the city capscity?

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Water Supply

2008-07-30 Thread Paul Pinigis
I just re-read your original question.  If I read it correctly, you
indicate that your demand point is below the curve, but the flow
measured during the test was less than the demand flow of your system.  

As long as you are below the curve you are fine.  The amount of flow at
the time of the test is irrelevant, it simply provides a point on your
curve.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Wednesday, July 30, 2008 1:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water Supply

I have tried a new flow test with two 2-1/2 openings flowing and the
pressure dropped off so that didn't work. I checked the coefficient and
it
is a .9. The hydrant does have a rounded inlet. I don't have play pipes
and
either does the city which is the only one that can do the test. I have
tried different heads and pipes and nothing will drop my GPM to below
the 31
gpm we are short. 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Wednesday, July 30, 2008 11:08 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water Supply

That was my first thought too.  Joe's been around and must have already
done
this.  Maybe he's having a bad day or there is more to the story.  

To answer Joe's question plainly, no.  The but is I never meet an AHJ
that
wouldn't give up 31gpm especially on a 500 hose allowance.  A fire pump
is a
tough sell for 31 gpm especially when the hose isn't used until the FD
arrives and they bring a pump.  I'd though, if as an AHJ, would make
sure
you really did practically max out pipe sizes.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Richard
Carr
Sent: Wednesday, July 30, 2008 11:43 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water Supply

If you plot it out on a curve you will have more than 1210 but at a
lower residual pressure.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[EMAIL PROTECTED]




-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Wednesday, July 30, 2008 11:58 AM
To: SprinklerFORUM
Subject: Water Supply

I have a project where the system demand with hose allowance exceeds the
city supply by 31 GPM. It's still under the curve but the city flow test
was
1210 and my system demand is 1241. Is there anything in the codes that
allows me to exceed the city capscity?

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


This email and any attached files are confidential and intended solely
for
the intended recipient(s). If you are not the named recipient you should
not
read, distribute, copy or alter this email. Any views or opinions
expressed
in this email are those of the author and do not represent those of the
company. Warning: Although precautions have been taken to make sure no
viruses are present in this email, the company cannot accept
responsibility
for any loss or damage that arise from the use of this email or
attachments.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Deperming Pier

2008-07-24 Thread Paul Pinigis

Please direct your questions about this installation to the engineer of record, 
Eric Shelton, P.E.

Thank you,
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
Hankins and Anderson


-Original Message-
From: [EMAIL PROTECTED] on behalf of Kurt Kingston
Sent: Thu 7/24/2008 10:51 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Deperming Pier
 
I have seen a nice dry standpipe system installation done by a
competitor using HDPE and fusion seal fittings a few years ago on a salt
water pier (Cap Sante Marina, Anacortes, WA.). I cannot remember the
specific brand now, but this link is something similar:
http://corrosion-products.com/PipingProducts/HDPE.htm
IMHO, it looked like using the right tool.
Good success,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
PO Box 128
Mt Vernon, WA 98273
ph (360)-848-9093 fax (360)-848-1072
 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, July 24, 2008 6:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Deperming Pier

I'd be concerned about two things with CPVC-
Effects of sunlight, even under the pier you'd likely get strong
reflections
off the water; and where are you getting 6 CPVC?
I have no idea if regular plumber's PVC would work; if you have a
low-pressure DPV, and you're looking at a 2.5 DPV as your activating
device
(and combo exhauster, it's a pretty big orifice) then wouldn't the air
never
be at high pressure and so it shouldn't be a problem to use PVC?

NFI, just a thought that would save my tax dollars versus SS316.

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, July 24, 2008 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Deperming Pier

What if you ran plastic, CPVC is approved for fire protection above
grade
per NFPA 13.  See 6.3 of NFPA 13, 2007.






Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rick
Green
Sent: Thursday, July 24, 2008 8:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Deperming Pier


I am installing a dry pipe system (no sprinklers) supplying four hose
valves
on a pier.

The dry pipe valve assembly is located in a heated area.  Extending out
from
the dry pipe valve assembly  is 6 galvanized steel pipe.  The steel
pipe is
routed below the pier out to the  location of four hose valves.

The pier is used for Deperming ships, submarines.

Deperming is a procedure for erasing the permanent magnetism from ships
and
submarineshttp://en.wikipedia.org/wiki/Submarines to
camouflagehttp://en.wikipedia.org/wiki/Camouflage them against
magnetic
detection vessels and enemy marine
mineshttp://en.wikipedia.org/wiki/Naval_mines.

Anyway, there is about a 200' section of the pier that requires that all
materials be non-magnetic.

*Galvanized steel pipe that NAVY specified obviously want work.

*CPVC plastic pipe will not work because installing dry system -
correct on this right?

*Provided them pricing for stainless steel, copper, brass and
now
they want pricing for Aluminum,.

So a few questions

o   Ever used aluminum pipe for sprinkler installations?

o   Is there some other pipe type that I am not thinking about

Help would be most appreciated.

Rick E. Green
District Manager
East Coast Fire Protection, Inc.
1113 Cavalier Boulevard
Chesapeake, Virginia 23323
757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell)
[EMAIL PROTECTED]

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fire Flow Calculation

2008-07-23 Thread Paul Pinigis
Nope, if you have a building that is not sprinklered in accordance with
NFPA 13 (and you don't because there are unsprinklered areas beyond
those that are allowed to be unsprinklered by NFPA 13) you have an
unsprinklered building.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 5:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation

It's for fire flow from hydrants. I guess I'm wondering if we can
pro-rate the unsprinklered percentage. If we use 50k sqft with no credit
for sprinklers and 300k sqft at a 75% reduction and add them together or
something to that effect. 

Ron
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Wednesday, July 23, 2008 1:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation

Tables B and C of the IFC ( I think) list the flows.  An intersting
question arises..., if it is not fully sprinkled... I believe you do not
get the nice reduction?.. Is this what you are looking for ?

R/

Matt 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:36 PM
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Calculation

Looking for help to determine required fire flow. New addition to
hospital is 200k sqft. 150k sqft existing building with 50k sqft of the
150k not sprinklered. Construction type is I-FR.

Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Institutional Sprinklers

2008-07-14 Thread Paul Pinigis
How about putting some indelible orange ink in the line so that the next
moron who opens the sprinkler becomes an oompa loompa? 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, July 14, 2008 3:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Institutional Sprinklers

Handcuff's ?? 


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Monday, July 14, 2008 3:52 PM
To: sprinklerforum@firesprinkler.org
Subject: Institutional Sprinklers

Problem; we have some institutional sprinklers in a holding cell at a
local
jail that repeatedly are getting knocked out by the temporary inmates.
Has
anybody come up with a good solution to this problem from our end;
specialty
sprinkler guards or anything?

 

Thank you in advance,

 

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130

   

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
5.10250e http://www.pctools.com/en/spyware-doctor-antivirus/





E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Backflow device and steel pipe

2008-07-02 Thread Paul Pinigis
But, ductile iron IS ferrous pipe!  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Wisneski
Sent: Wednesday, July 02, 2008 8:21 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Backflow device and steel pipe

Well forumites, I've gat a new one (to me).

Customer wants a small anti-freeze system on a loading dock. The
existing
system is a steel pipe system with a double check backflow at the
service
entry. 

Normally I would just tap into the closest main (5 feet away), drop down
to
a reduced pressure backflow and install an expansion tank and the eight
head
anti-freeze system.

The water purveyor now tells me that is unacceptable. They want the
anti-freeze system tied into the ductile iron pipe at the service
entrance,
before the existing double check, and fed with non ferrous pipe. They
say
they do not want any type of backflow device fed with black steel pipe.

This, I believe, is not a code issue.

Has anyone run into this situation before?

Thanks in advance,

 Mike Wisneski

 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: PIV 40ft from Building

2008-06-18 Thread Paul Pinigis
As the story was told to me, this dates back to the first iron-framed
buildings with brick exterior walls. The buildings were generally
walk-ups (pre-elevator days) so they were up to four stories tall.  The
problem was that the iron would expand in a fire and push outward on the
walls until the brick failed and collapsed.  The 40-foot distance was
considered to be out of reach of the falling brick and would allow the
fire department to shut off the water to conserve water for manual fire
fighting.  

Might be true, might be a campfire story.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Sornsin
Sent: Wednesday, June 18, 2008 10:43 AM
To: sprinklerforum@firesprinkler.org
Subject: PIV 40ft from Building

Forum:

Anyone know the reason WHY PIVs are to be located at least 40 ft. from
the building (on a fire service line piped into the building)?

I have heard some theories - like to keep the valve free from a
collapsing wall.  But I am curious if any of you have any definitive
explanations for that number.  Why not 30 ft.? Why not 50 ft.

We are dealing with an AHJ who is requiring we pipe an underground an
additional 200+ ft. around a corner just so our PIV can be at least 40
ft. from the building.  Otherwise, if we pipe straight out the building,
the public right-of-way is such that we'd be only 31 ft. from the
building with the PIV.  This is not good enough for this gentleman
since, as he says, it is POSSIBLE for you to get it 40 ft. away (with
the 200+ ft. of underground).  If there was no other way, he would have
allowed the 31 ft. separation.
 

Frustrated-in-Fargo, PE
Fire Protection Engineer 
Ulteig Engineers, Inc. 
3350 38th Avenue S. 
Fargo, ND 58104-7079

Direct:701. 280.8591 
Fax:701.280.8739 
Cell:701.371.5759 

[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]  
www.ulteig.com http://www.ulteig.com/  

Cofidentiality Notice

This message may contain privileged and confidential information. If you
think, for any reason, this message may have been addressed to you in
error, you   must not disseminate copy or take any action in reliance on
it, and we would ask you to notify me immediately by return email to
[EMAIL PROTECTED] 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Sectional Valves...

2008-05-21 Thread Paul Pinigis
If the closure of those valves will impair the operation of the system
(which I believe they will) they need to be monitored.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Wednesday, May 21, 2008 10:40 AM
To: sprinklerforum@firesprinkler.org
Subject: Sectional Valves...

 

I think I asked this already... and apologize for regurgitating it!  I
have a bldg. that is 'U-shaped' in nature.  The system is of CPVC in
nature - fairly small.  Prior to going into the 'legs' of the 'U' - the
contractor wants to have (2) ball valves installed to isolate each wing
for maintenance purposes.  Do these ball valves need to be of a
'monitored' (wired to panel) type or can they be just run-of-the-mill
ball valves?

 

Imho - I believe they should be 'monitored' valves.  Thanks!

 

R.F.P. Chuck

 


No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.21/1458 - Release Date:
5/21/2008
7:21 AM
 
  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
Look at the cut sheet on the BFP.  Some BFPs require a significant
amount of pressure to open at very low flows.  For example, an 12 Ames
2000SS requires almost 6 psi to operate at very low flow so it can sit
there all day with an upstream pressure nearly 6 psi higher than the
system side pressure.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: sprinklerforum@firesprinkler.org
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
If water was flowed on the system side of the BFP there can be a lower
pressure on the system side vs. the supply side due to the on-off
action of some axial-check BFPs.  This is not the same phenomenon as the
pressure difference across an ACV because the ACV uses a simple
side-hinged check.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Friday, May 09, 2008 3:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Change in static pressure

The BFP should trap the highest pressure on the system side so that
the up and down fluctuations will happen on the supply side. This will
read the same as the two gages on an alarm check valve when it is
acting as the only system/supply check. The water tower seems the
culprit. The elevation difference accounts for 7.4 psi. The remaining
10.6 psi could be the tank if the before refill/after refill elevation
inside the tank is 24.5 feet.



On Fri, May 9, 2008 at 11:59 AM, Dewayne Martinez [EMAIL PROTECTED]
wrote:
 Thanks,
 I will look into the cut sheet.  The fitter preformed an alarm test so
 only a small amount of water was flown.

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Paul
 Pinigis
 Sent: Friday, May 09, 2008 1:22 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Change in static pressure

 Look at the cut sheet on the BFP.  Some BFPs require a significant
 amount of pressure to open at very low flows.  For example, an 12
Ames
 2000SS requires almost 6 psi to operate at very low flow so it can sit
 there all day with an upstream pressure nearly 6 psi higher than the
 system side pressure.

 Paul J. Pinigis, P.E.
 Chief Life Safety Engineer

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
 Martinez
 Sent: Friday, May 09, 2008 1:55 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Change in static pressure

 I have a job site which is 10ft higher than the water supply.  A gauge
 on the water supply hydrant reads 55 PSI static pressure while two
 gauges on the system riser after the BFP read 37 PSI?  The total
 elevation change between the system gauges and the supply gauge is
about
 17ft.  Why would there be a 18 PSI difference between the gauges when
 elevation only accounts for 7.36 PSI?
 I confirmed with the city that there are no shut valves.  Any
thoughts?
 Thanks,
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Hay Bale/Cube Storage

2008-03-17 Thread Paul Pinigis
Class III, ordinary combustibles.  See chapter 14 of the 2007 NFPA 13
for design density curves. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr
Sent: Sunday, March 16, 2008 5:28 PM
To: American Fire Sprinkler Association
Subject: Hay Bale/Cube Storage

Forum,

 

What commodity class would hay bales in solid piles to 20 feet in height
fall under?

This is a fully enclosed structure.

Thanks in advance,
Ed Cyr

Alpha Fire Sprinkler Corp.



 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fuel Tank Rooms

2008-03-10 Thread Paul Pinigis
Why?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Denhardt
Sent: Monday, March 10, 2008 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fuel Tank Rooms

NFPA 13 - 2007 

I would try Section 21.6: .30gpm/sq.ft. over 2500 sq.ft.  100 sq.ft. per
sprinkler maximum

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Phelan
Sent: Monday, March 10, 2008 1:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Fuel Tank Rooms

How does the group feel on the occupancy classification of a rated room
in a building that contains a 275 Gal #2 Fuel tank for the rooftop
generator?  The room is on the ground level and the tank is 130 feet
above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room
with a single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that
the tank is not combustible, just the product in it ...  Im leaning
towards a EH designation in the event of fire the fuel would be more
than capable of supporting combustion.  At the very least I dont see the
current configuration as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fuel Tank Rooms

2008-03-10 Thread Paul Pinigis
I would agree with OH2 (or even OH1).  It is a combustible liquid in a
closed system.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Phelan
Sent: Monday, March 10, 2008 1:51 PM
To: sprinklerforum@firesprinkler.org
Subject: Fuel Tank Rooms

How does the group feel on the occupancy classification of a rated room
in a building that contains a 275 Gal #2 Fuel tank for the rooftop
generator?  The room is on the ground level and the tank is 130 feet
above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room
with a single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that
the tank is not combustible, just the product in it ...  Im leaning
towards a EH designation in the event of fire the fuel would be more
than capable of supporting combustion.  At the very least I dont see the
current configuration as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: BASIC HYDRAULICS

2008-02-28 Thread Paul Pinigis
Elevation still affects the pressure in a closed system.  If the water
is static in a pressurized system the pressure is the same throughout
the system only at a constant elevation.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Thursday, February 28, 2008 11:55 AM
To: sprinklerforum@firesprinkler.org
Subject: BASIC HYDRAULICS

Someone educate me or re-educate me on basic hydraulics, engineering not
necessarily sprinkler hydraulics. I understand the difference between
static pressure and residual pressure while flowing some amount and how
gravity losses come into play with increasing elevation. However I have
the notion that a closed system when pressurized has equal pressure thru
the entire system such as when testing a sprinkler system at 200 psi.
The pressure in the closed system pumped up to 200 psi is 200 psi
throughout regardless of elevation?
 
Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dormitory Bunk Beds

2008-02-26 Thread Paul Pinigis
8.5.5.3.2  Sprinklers shall not be required under obstructions that are
not fixed in place such as conference tables.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
Sent: Tuesday, February 26, 2008 4:05 PM
To: sprinklerforum@firesprinkler.org
Subject: Dormitory Bunk Beds

I have asked an interesting question today by a general contractor and
need some assistance.

 

A local college dormitory is undergoing some renovations and the
question was asked about double or full size Bunk Beds (wider than 4'-0)
being used in the rooms.

The local fire marshal has asked about sprinkler protection below the
upper bunk. I am assuming an existing structure at this point and the
design will call for HSW sprinklers on exposed pipe.

My thought would be to locate the sprinkler head on the opposite wall.
Now keep in mind that the furniture may be movable. 

 

I do not believe this scenario is addressed in NFPA 13, 13R or D.
Platforms, Cutting tables and duct wider than 4' are addressed.

 

Any thoughts or comments would be greatly appreciated.

 

Thank you.

 

G. Tim Stone

 

G. Tim Stone Consulting, LLC 

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

117 Old Stage Rd. - Essex Jct., VT. 05452

TEL: (802) 434-2968  Fax: (802) 434-4343

[EMAIL PROTECTED]

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Gaggle of closets

2008-02-22 Thread Paul Pinigis
Don't you just love it when the letter of the code works in your favor.
I really don't think that this is what the NFPA 13 committee had in mind
when they developed that section.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, February 22, 2008 5:05 PM
To: sprinklerforum@firesprinkler.org
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according 
to NFPA 13. On the first level, there is a room which contains 55 - 
3'x5' tenant storage closets (mostly filled with shelves). These 
would need to be sprinklered, which is fine, but the issue comes in 
the hydraulics. Section 14.4.4.4.2 states that closets with a single 
sprinkler may be omitted from the calculation. There could be up to 
47 closets in the remote area. I have used this exception numerous 
times, but never in this quantity. The standard says nothing to the 
contrary, so I could eliminate 47 sprinklers in the remote area 
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: General Seismic Question

2008-02-20 Thread Paul Pinigis
1. No, that is the responsibility of the engineer and the project design
team.
2. Yep, that is a clear change order.
3. Check your contract for this one.  He most likely has to pay for work
done and materials fabricated. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Wednesday, February 20, 2008 11:00 AM
To: sprinklerforum@firesprinkler.org
Subject: General Seismic Question

We have a job that we bid which excluded seismic bracing, we are suppose
to start hanging pipe on Monday the 25th. The GC is now telling us that
we need to include seismic and he expects us to eat the cost, if we
don't he's going to use the 2nd place bidder. He says that it was our
responsibility to determine if seismic was required or not. 

1.  Is it ever the sprinkler man's job to determine if seismic is
required? I think not...
2.  If you exclude items in your bid and are awarded the contract
isn't
a change order at this point a no brainer?
3.  Can he legally ditch us at this point and go to the number 2
bidder,
we already have pipe fabricated?

 

Regards,

 
http://www.firstdefensefire.com/  

 

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Diesel vs Electric

2008-02-15 Thread Paul Pinigis
We have found that a diesel pump alone is more cost effective than an
electric with a gen set.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, February 15, 2008 7:32 AM
To: sprinklerforum@firesprinkler.org
Subject: Diesel vs Electric

Hello sprinklerforum,

  I am looking for opinions on installing a Diesel fire pump Vs
installing
  an Electric fire pump and Gen Set. I have a location that is being
  cut loose from the Site Wide fire pump loop now owned by others.

-- 
Best regards,
 Charles  mailto:[EMAIL PROTECTED]
Coastal Fire Protection

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Re[2]: Who's the most important person?

2008-02-06 Thread Paul Pinigis
Idiots are important too! 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, February 06, 2008 4:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Re[2]: Who's the most important person?

So why is it that we're always wondering why we have so many idiot
clients ... ??   Oh, never mind. :o)

Steve Leyton
Protection Design  Consulting


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, February 06, 2008 1:23 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Re[2]: Who's the most important person?

You have all missed it.  The CLIENT is the most important; without him
you have no project.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown (TECH- GVL)
Sent: Wednesday, February 06, 2008 4:08 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Re[2]: Who's the most important person?

You guys do not understand the Golden Rule.  HE WHO HAS THE GOLD
RULES!
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matsuda,
Richad
Sent: Wednesday, February 06, 2008 3:42 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Re[2]: Who's the most important person?

I'd like to vote, tooonly my opinion.

1. The PE or architect or sprinkler designer does his work on paper.
2. The AHJ or consulting engineer approves the paper submittal.
3. The field crew installs the project based on the paper plans, but
they have the ability to make desisions based on their knowledge of what
is required, and perhaps make appropriate corrections before the city
inspector finds these errors. 
4. The city inspector who approves/disapproves the installation based on
the approved plans and his knowledge of what is required.

The most important people are the field crew and city inspectors because
they ultimately see and approved the completed project regardless of
what is done on paper in Items # 1 and 2. 

Heck, I'm only a plan reviewer...and I have the upmost respect for the
knowledgable field guy who finds and corrects all the mistakes that I
made during my paper plan review. Train them, pay them, and keep them in
your company cause they can make or break you.

rick matsuda, city of dallas

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, February 06, 2008 3:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Re[2]: Who's the most important person?

Actually the question was a serious one.  I am trying to separate the
components of successful companies into several categories - perhaps I
should have included the fitter crew also.  Maybe this one of those
chain is no stronger than the weakest link scenarios.

Maybe there's no ready answer to the question - I'll go back and sit
down now.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: 3 alarm Fire @ Monte Carlo now in las vegas

2008-01-25 Thread Paul Pinigis
It looks that way.  But WHY?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... 
Sent: Friday, January 25, 2008 3:11 PM
To: sprinklerforum@firesprinkler.org
Subject: 3 alarm Fire @ Monte Carlo now in las vegas

it is early to say, but I will anyway...
sounds like a sprinkler
did not get water on the fire.

scot deal
excelsior fire
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: MIC Testing

2008-01-18 Thread Paul Pinigis
Will they test the pipe too?  I only know of them testing the water and the 
scale, not the quality of the pipe.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Terri Leyton
Sent: Friday, January 18, 2008 11:08 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: MIC Testing

http://www.huguenotlabs.com/
These guys are pretty good.

Terri Simmons Leyton
PROTECTION DESIGN  CONSULTING
Ph:  858-751-2930 - ext. 101
Fax:    858-751-2933
Cell:  619-871-8450

Go CHARGERS!  We take care of our KIDS!


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, January 18, 2008 6:06 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: MIC Testing

There is a forensic metallurgist in Northern Virginia that I have used a
few times.  I am looking for his card, but no luck yet. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, January 17, 2008 9:52 PM
To: sprinklerforum@firesprinkler.org
Subject: MIC Testing

Where do you send pipe for MIC testing?
 
Forest Wilson
Cherokee Fire



**Start the year off right.  Easy ways to stay in shape.

http://body.aol.com/fitness/winter-exercise?NCID=aolcmp0030002489
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: MIC Testing

2008-01-18 Thread Paul Pinigis
There is a forensic metallurgist in Northern Virginia that I have used a
few times.  I am looking for his card, but no luck yet. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, January 17, 2008 9:52 PM
To: sprinklerforum@firesprinkler.org
Subject: MIC Testing

Where do you send pipe for MIC testing?
 
Forest Wilson
Cherokee Fire



**Start the year off right.  Easy ways to stay in shape.

http://body.aol.com/fitness/winter-exercise?NCID=aolcmp0030002489
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: One Fire Pump Serving Multiple Buildings

2008-01-17 Thread Paul Pinigis
I have done this several times.  It is analogous to single pump house
feeding a campus, but you happen to have the pump in one of the
protected buildings instead.  Just as with a pump house, you assume a
single fire condition.   

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, January 17, 2008 10:41 AM
To: sprinklerforum@firesprinkler.org
Subject: One Fire Pump Serving Multiple Buildings

Are there any codes regulating the use of one fire pump to serve
multiple 
building?  Do you assume only one fire condition? 

John Kaminski



This email is intended for named recipients only.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Great Forum Advice...

2008-01-16 Thread Paul Pinigis
Maybe we can get the Union and the class-action lawyer listed on the
State Department's list of terrorist organizations.  It sounds like
their tactics are awfully similar to those of other extremists. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Terri
Leyton
Sent: Wednesday, January 16, 2008 1:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Great Forum Advice...

Hi All,

I would like to gather some opinions on a rather sensitive subject.
We have a very long time, good client, who has been in the sprinkler
business since he joined the Union in 1961.

 

His Contracting Company is now open shop and has been since 1994.  He
and several other San Diego area contractors have been arbitrarily sued
by Local 669, allegedly for violations of overtime and prevailing wage
obligations.   The MO has been to find ex-employees of these firms and
essentially sponsor class-action law suits against these firms, even
though there may not be evidence of any wrong-doing.  In fact, in our
friend's case, the judge has dropped the union from the suit as there is
no substance to any claims of theirs.  However, the suits have been
allowed to proceed as class actions and it may be that 669 continues to
fund the plaintiff's counsel; the latest tactic was that clients of this
firm have received letters notifying them that they have or may be named
as John Does in the litigation.

 

There appears to be no merit to these suits and the plaintiff's tactics
are simply to bleed the defendants financially and it's working.  Now,
with GC's and developers being put on notice, there isn't much chance
that these companies can continue  doing business under current
circumstances.  According to our friend's attorneys, it's all legal -
perhaps in equal parts because it's happening as a class action and
because it's in California.

 

This is now affecting other companies - like OURS.  And their other
vendors and subs, such as fabricators and underground utilities
contractors.  Any similar experiences?  Any advice?

 

 

Terri Simmons Leyton

PROTECTION DESIGN  CONSULTING

8849-B Complex Drive

San Diego, CA 92123

-

Ph:  858-751-2930 - ext. 101

Fax:858-751-2933

Cell:  619-871-8450

 

The height of your accomplishments will equal the depth of your
convictions. --William F. Scolavino

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Room Design

2007-12-21 Thread Paul Pinigis
If the doors are open at the time of your visit, I think it is safe to
assume that they will be propped open at other times as well (unless of
course they were temporarily propped open to move equipment in or out).


Merry Christmas everyone!

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, December 21, 2007 10:14 AM
To: sprinklerforum@firesprinkler.org
Subject: Room Design

When you are performing an inspection of a system calculated using the
room design approach, how do you handle all of the doors that are
propped open?

Or, how do you calculate these systems?  Do you always go with the extra
two sprinklers and assume the doors will be held open?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Room Design

2007-12-21 Thread Paul Pinigis
I am not sure if I understand your question completely, but here is my attempt 
at an answer.  The remote area is the actual physical area and not the 
hydraulic area.  For example, consider a 22'x22' room with four sprinklers on 
14' centers, the actual physical area is 484 sq. feet, but the hydraulic area 
is 784 square feet.  Only 484 sq. ft. is in the design area.  

Have I interpreted your question properly?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jason Norton
Sent: Friday, December 21, 2007 1:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

While we are on this topic...We have a small debate in our office regarding the 
density/area method.  Some say to ignore the walls completely through the 
entire calculation process, just like the example that NFPA 13 describes (which 
works great for a the typical warehouse with equal sprinkler spacing). Others 
say ignore the walls with regard to the general location of the remote area 
(1.2 rectangle) and then use the walls to determine the actual square footage 
of the remote area and to determine the actual gpm required from each sprinkler 
within the remote area. What do you all say? 

Jason

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, December 21, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

I can't see a good reason for NFPA to nix the room design method - I've seen 
enough locations where the self-closing doors actually remain closed. But I 
can't see a contractor willingly avoid the room design either - not without 
potentially losing more work to the other guy.

A classic example of why NFPA 13 is a minimum standard; and why (many times) 
there should be a third party taking responsibility for the design. Say, like 
an engineer of record for instance - one that knows what's going on, that is.

Mark 
 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... 
Sent: Friday, December 21, 2007 9:53 AM
To: sprinklerforum@firesprinkler.org
Subject: Room Design

propped open doors?
propped open self-closing doors?
that IS reality.

that is why the Room Design method
  has to wake up and smell the coffee.
not that the Room Design method is bad in intention.
  one, two,  three sprinklers kabosh most LH/OH fires.
just that there are some bad assumptions
  to the Room Design method.
  Like doors being closed.


scot deal
excelsior fire
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Standpipe Requirements

2007-12-20 Thread Paul Pinigis
That is going to be in the building code.  If you are using the IBC, the
height of the building dictates the necessity of standpipes. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Thursday, December 20, 2007 11:23 AM
To: sprinklerforum@firesprinkler.org
Subject: Standpipe Requirements

I have a question for anyone working today. There is a code somewhere
that
states when a standpipe must be used. I have searched through NFPA 14
and 13
and can not find the code. Does anyone know what and where that
information
is?

Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Flow test effective point.

2007-12-14 Thread Paul Pinigis
Yes, you must correct for elevation. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, December 13, 2007 5:52 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow test effective point.

I thought I understood this, but maybe not. When determining the 
effective point for a hydrant flow test, I was told that it is at the 
junction of the flowing and non-flowing water. (for the purposes of 
this discussion, let's assume that we are talking about a single 
main, fed from both directions, with hydrants on branches off the 
main. Pressures are read at one hydrant and another single hydrant is 
flowed) If this is the case, then the effective point of of the flow 
test would be at the junction of the main and the branch to the 
hydrant where the pressures are read. However, this junction occurs 
underground. If we assume that the gauge on the hydrant is 1'-6 off 
the ground and the main is 5 ft underground, this would mean that the 
pressures are read 6.5 ft above the effective point. The pressures at 
the effective point would be 2.8 psi greater than those read at the 
hydrant. Is or should a correction be included?

This makes a difference on programs such as Autosprink where you draw 
a 3D model of the underground system and insert a supply at the 
effective point.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dick Patton

2007-12-12 Thread Paul Pinigis
Yes, I got a copy of his report from the 1970s.  The current cost, with
inflation, is actually $1.71 per square foot, but he took credit for
reducing the amount of fireproofing on the structure as a reduction in
the cost of his system.  He provided no details to show a difference
between his design and any NFPA 13 design. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, December 12, 2007 4:46 PM
To: sprinklerforum@firesprinkler.org
Subject: Dick Patton

Anyone ever get a reply to their request from Richard Dick regarding
his $0.38 per sq. ft. hospital design?
 
Steve Leyton
PROTECTION DESIGN  CONSULTING
8849-B Complex Drive
San Diego, CA 92123
-
Ph:  858.751.2930 - Ext. 102
Fax:858.751.2933
Cell:  619.972.5696
 
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dick Patton

2007-12-12 Thread Paul Pinigis
Definitely Turd polishing. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, December 12, 2007 5:28 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dick Patton

Hmmm, you want to write him back and ask him about the particulars or
does this fall into the category of polishing a turd?

(Sorry Munce - for more on polishing, see AFSA's seminar program ...)
:o)

Steve Leyton
Protection Design  Consulting


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, December 12, 2007 1:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dick Patton

Yes, I got a copy of his report from the 1970s.  The current cost, with
inflation, is actually $1.71 per square foot, but he took credit for
reducing the amount of fireproofing on the structure as a reduction in
the cost of his system.  He provided no details to show a difference
between his design and any NFPA 13 design. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, December 12, 2007 4:46 PM
To: sprinklerforum@firesprinkler.org
Subject: Dick Patton

Anyone ever get a reply to their request from Richard Dick regarding
his $0.38 per sq. ft. hospital design?
 
Steve Leyton
PROTECTION DESIGN  CONSULTING
8849-B Complex Drive
San Diego, CA 92123
-
Ph:  858.751.2930 - Ext. 102
Fax:858.751.2933
Cell:  619.972.5696
 
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Wow

2007-11-21 Thread Paul Pinigis
I reviewed some of his writings, and he has an obvious bias against just
about everything.except heat detectors.  I wonder if he is one of
those guys who sells the wind-up heat detectors?

Most of his statistics appear to be unfounded, and unsubstantiated.  He
is also part of an organization the is out to expose the evils of the
ionization smoke detector...their message is very one-sides, but not
completely inaccurate.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Wednesday, November 21, 2007 9:12 AM
To: sprinklerforum@firesprinkler.org
Subject: Wow

http://www.expertclick.com/NewsReleaseWire/default.cfm?Action=ReleaseDet
ailID=18844
 
 
What a way to start the day...
 
 
 
Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Wow

2007-11-21 Thread Paul Pinigis
I just got a return email from Mr. Patton.  He is going to send me a copy of 
his report on the 35 cent design.  I will disseminate what I learn from it to 
the forum in a couple of weeks.  I am imagining thousands of water balloons 
tied to the ceiling, but I think the labor for that might exceed 35 cents per 
square foot. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Wednesday, November 21, 2007 1:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Wow

If you're talking about Richard Dick Patton, I didn't know he was selling 
kitchen hood systems.  I just thought he was a loony.

I kinda' like conspiracy theorists though.  You can usually un-piece their 
strategy by disconnecting the facts that are strung together to form their 
theory.   Dick says he designed a 1.2 million s.f. medical center for 35 cents 
per s.f.  I think we can pretty much stop reading right there.

There is a troubling aspect to seeing this guy's rantings in print however, and 
that is that people who would seize any idea that they think would make 
sprinklers cheaper (i.e. the NAHB, for ex.) will give him a venue and an 
audience.  Our good friend, the late Bob Caputo and my SoCal buddy Ken Wagoner 
have both had their day with this fellow and they came out of the experience 
with anger issues and a foul odor about them.

Steve Leyton
Protection Design  Consulting


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Cabral
Sent: Wednesday, November 21, 2007 6:34 AM
To: sprinklerforum@firesprinkler.org
Cc: Matt Willis
Subject: Re: Wow

This guy is selling Fire Extinguisher. Kitchen Fire Suppression Systems. . . 
his answer to the US Fire problem. Talk about self serving. . .
--
Mike Cabral

 Matt Willis [EMAIL PROTECTED] wrote: 
 http://www.expertclick.com/NewsReleaseWire/default.cfm?Action=ReleaseDet
 ailID=18844
  
  
 What a way to start the day...
  
  
  
 Matthew J. Willis
 Living Water Fire Protection, LLC.
 1160 McKenzie Rd.
 PO Box 877
 Cantonment, FL. 32533
 850-937-1850 Voice
 850-937-1852 Facsimile
 [EMAIL PROTECTED]
  
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

RE: 13-R Anti freeze conversions

2007-10-25 Thread Paul Pinigis
I assume that these systems are not CPVC since CPVC is incompatible with
most antifreeze. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ford,
Charles
Sent: Thursday, October 25, 2007 3:38 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13-R Anti freeze conversions

We have been asked to convert many (100+) existing 13-R systems to
anti-freeze. The valve groups are
installed in unheated garages (with heat tape) but the garages are
sprinklered and freeze
occasionally. Garages cannot be isolated for dry sidewalls due to
configuration. All homes are owned
by a single company. 

My basic question: Is this a good idea? Wouldn't it be cheaper in both
the long and short run to heat
garages to 40+ F? These are in the NE USA but below the Mason Dixon
line. Comments welcome.   


Burton Ford
SET, CFPS
Member AFAA
[EMAIL PROTECTED]
267-487-1000
Fax 267-487-1010

This e-mail transmission contains information that is intended to be
confidential and privileged.  If
you receive this e-mail and you are not a named addressee you are hereby
notified that you are not
authorized to read, print, retain, copy or disseminate this
communication without the consent of the
sender and that doing so is prohibited and may be unlawful.  Please
reply to the message immediately
by informing the sender that the message was misdirected.  After
replying, please delete and otherwise
erase it and any attachments from your computer system.  Your assistance
in correcting this error is
appreciated.  Thank you.  Cintas Corporation

 -Original Message-
From:   [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]  On
Behalf Of A.P.Silva
Sent:   Thursday, October 25, 2007 12:37 PM
To: sprinklerforum@firesprinkler.org
Subject:Fire Department boost pressure

This is two questions in one posting. A two for one deal.

I'm designing a sprinkler system for a grain elevator that has been
taken
out of service, and now used as a museum. It will be cleaned and there
will
be no more grain. This building has a footprint of approx. 2000 sf. So
crawlspace and main floor are 2000 sf each. The area housing the 7 grain
bins is about 80 feet high and has a foot print of approx. 1000 sf
(included
in the main floor 2000 sf). At the very top there is a lower penthouse
and
upper penthouse (about 300 sf each). The building area is small, but due
to
sloped roofs and obstructions, requires about 110 sprinkler heads.

The first question: Although it is classified as a museum, I'm designing
it
for OH1 occupancy. The entire building is exposed wood construction and
very
dry. If there is a fire the fuel load is very high. Any comments?

Now there is a crawlspace area under the bins that is combustible and
not
accessible. The owner does not want this area to be sprinklered. So
kicks in
the 3000 sf requirement. 

Second question: Should I include heads a diffent levels in my calcs.?
The
city supply (110 static pressure) is enough to supply about 30
sprinklers at
different levels at the top (excluding the penthouses which are not open
to
the rest of the building). Should I be includng additional sprinklers
from
the penthouses and lower levels?

If I did include additional heads, the city supply is insufficient. But
the
owner (who is the City) has told me that if the city supply is not
enough,
it will be boosted by the responding fire department and they will issue
a
variance to that effect.

So the third question (I cheated there were three), which would apply to
other buildings also that have high pressure water supply. Do I need a
pressure reducing valve? The fire dept. boost is typically over 100 psi.


Tony  

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not
a named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be
unlawful.  Please reply to the message immediately by informing the
sender that the message was misdirected.  After replying, please delete
and otherwise erase it and any attachments from your computer system.
Your assistance in correcting this error is appreciated.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org

RE: UNDERGGROUND FIRE MAIN TESTING

2007-10-11 Thread Paul Pinigis
Pressure is pressure, but do you really want to test the integrity of
plastic fittings with a compressible gas?  A failure could produce a
most interesting rocket from a piece of pipe.  If you must use a gas,
why nitrogen, why not compressed air (not suggesting that either is a
good idea)?  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Loren
Johnson
Sent: Thursday, October 11, 2007 12:23 PM
To: Sprinkler Forum
Subject: UNDERGGROUND FIRE MAIN TESTING

Forum:

We have a situation that just came up.here's the
quick question side of things:

Can listed plastic underground fire main piping be
tested with nitrogen instead of the typical
hydro-static water method?  I've always been told this
is not acceptable, and there are no sections on the
test form that indicate this to be an option. In
addi-tion, since FM Global is the insuance carrier for
this project, there is a very strong possibility the
installation would be unacceptable when field
in-spected.  

Thanks in advance.


Loren Johnson
Peoria, IL 


 


Check out the hottest 2008 models today at Yahoo! Autos.
http://autos.yahoo.com/new_cars.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: [NJFireSafety] NASFM Code Enforcement Bulletin again

2007-10-10 Thread Paul Pinigis
According to this approach, my office is an H occupancy.  There is not
separation of my office from the rest of the spaces on this floor and we
have hundreds of chairs and several couches.  I do believe that we have
more than 250 pounds of polyurethane foam in the fire area.  Now I am
scared, I had no idea that I was entering a death trap every morning!
And, my God, I have upholstered furniture in my home...how
irresponsible!  

Is there any loss history to support his assertion that a furniture
showroom cannot be protected as a mercantile occupancy? 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, October 10, 2007 10:38 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: [NJFireSafety] NASFM Code Enforcement Bulletin again

Seems quite a stretch to call polyurethane a chemical in order to  
call it a flammable solid thus making the warehouse an H occupancy.
I would also think any group A plastic could fall into this same  
approach.  Didi the occupants have any trouble getting out - NO so  
why impose all the other requirements such as a much tougher egress  
criteria?  This is nuts.  Why not attack the size of the warehouse  
before sprinklers are required based on heat release and flame spread

Also do you have any data on the set-up of the flame test.  A burn  
rate of 0.1 inch per second is slower than a class II commodity for  
rack fires (excluding initial burn time).

Roland

On Oct 10, 2007, at 6:14 AM, John Drucker wrote:

 The list server stripped the file, heres the link;


 http://www.firemarshals.org/mission/catastrophic/ 
 furniture_stores_wareho
 uses.asp

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of John
 Drucker
 Sent: Wednesday, October 10, 2007 9:12 AM
 To: sprinklerforum@firesprinkler.org
 Subject: FW: [NJFireSafety] NASFM Code Enforcement Bulletin

 Forum Members,

 Thought this may be of interest to you.

 John Drucker

 

 From: [EMAIL PROTECTED]  
 [mailto:[EMAIL PROTECTED]
 On Behalf Of Robert J Davidson
 Sent: Wednesday, October 10, 2007 8:16 AM
 To: [EMAIL PROTECTED]
 Subject: [NJFireSafety] NASFM Code Enforcement Bulletin





 Attached is a copy of a code enforcement bulletin from the National
 Association of State Fire Marshals concerning upholstered furniture.







 Robert J Davidson

 Fire  Life Safety Consultant

 Davidson Code Concepts, LLC

 45 Colonial Drive

 Tinton Falls, NJ 07753

 732-643-1799 phone/fax

 [EMAIL PROTECTED] mailto:[EMAIL PROTECTED]

 www.davidsoncodeconcepts.com http://www.davidsoncodeconcepts.com/





 This message contains confidential information, intended only for the
 person(s) named above, which may also be privileged. Any use,
 distribution, copying or disclosure by any other person is strictly
 prohibited. In such case, you should delete this message and kindly
 notify the sender via reply e-mail. Please advise immediately if  
 you or
 your employer does not consent to Internet e-mail for messages of this
 kind.



 __._,_.___
 Messages in this topic
 http://groups.yahoo.com/group/NJFireSafety/message/ 
 5282;_ylc=X3oDMTM0Mj
 NxNTY1BF9TAzk3MzU5NzE0BGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBG1z

 Z0
 lkAzUyODIEc2VjA2Z0cgRzbGsDdnRwYwRzdGltZQMxMTkyMDE5MTM2BHRwY0lkAzUyODI-

 
 (1) Reply (via web post)
 http://groups.yahoo.com/group/NJFireSafety/ 
 post;_ylc=X3oDMTJwMG5la2RyBF
 9TAzk3MzU5NzE0BGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBG1zZ0lkAzUy

 OD
 IEc2VjA2Z0cgRzbGsDcnBseQRzdGltZQMxMTkyMDE5MTM2? 
 act=replymessageNum=5282
 | Start a new topic
 http://groups.yahoo.com/group/NJFireSafety/ 
 post;_ylc=X3oDMTJlZzdqNGxkBF
 9TAzk3MzU5NzE0BGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBHNlYwNmdHIE

 c2
 xrA250cGMEc3RpbWUDMTE5MjAxOTEzNg--
 Messages
 http://groups.yahoo.com/group/NJFireSafety/ 
 messages;_ylc=X3oDMTJlb3A4bW
 poBF9TAzk3MzU5NzE0BGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBHNlYwNm

 dH
 IEc2xrA21zZ3MEc3RpbWUDMTE5MjAxOTEzNg--  | Members
 http://groups.yahoo.com/group/NJFireSafety/ 
 members;_ylc=X3oDMTJlZDBlaGh
 rBF9TAzk3MzU5NzE0BGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBHNlYwNmd

 HI
 Ec2xrA21icnMEc3RpbWUDMTE5MjAxOTEzNg--
 Yahoo! Groups
 http:// 
 groups.yahoo.com/;_ylc=X3oDMTJkbmloMWEyBF9TAzk3NDc2NTkwBGdycElkA
 zUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMTk

 yM
 DE5MTM2
 Change settings via the Web
 http://groups.yahoo.com/group/NJFireSafety/ 
 join;_ylc=X3oDMTJmN3RtaGg1BF
 9TAzk3NDc2NTkwBGdycElkAzUxMTQ4MTQEZ3Jwc3BJZAMxNzA1MDYwNjgyBHNlYwNmdHIE

 c2
 xrA3N0bmdzBHN0aW1lAzExOTIwMTkxMzY-  (Yahoo! ID required)
 Change settings via email: Switch delivery to Daily Digest
 mailto:[EMAIL PROTECTED] Delivery:
 Digest  | Switch format to Traditional
 mailto:[EMAIL PROTECTED]  
 Delivery
 Format: Traditional
 Visit Your Group
 http://groups.yahoo.com/group/ 
 NJFireSafety;_ylc=X3oDMTJkZGFpa3IxBF9TAzk
 

RE: Owner's Information Certificate

2007-08-03 Thread Paul Pinigis
That depends upon the source of that information that he has
interpreted.  His property and casualty insurer (FM, IRI, etc.) may have
emphasized the property protection aspects of an NFPA 13 system since
they do not insure human life.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, August 03, 2007 3:46 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Owner's Information Certificate

Can you believe this gentleman told me that he had been told 20 times
that
NFPA 13 systems protect property only and not life safety? This is a
normal
intelligent businessman who said this?

No longer fuming, but wanting to go home and boss my dog around,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: Friday, August 03, 2007 2:42 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Owner's Information Certificate

Greg,

It would be good to mention where the OH2 requirement came from.


At 03:33 PM 8/3/2007, you wrote:
This letter is to reiterate the fact the sprinkler system in your new
building is designed and installed for Ordinary Hazard Group II
occupancy.
We have installed the system per approved drawings with some small
modifications as required per jobsite conditions.

Please note that your future tenants should be advised that if they use
the
building for storage of commodities, storage heights or storage
arrangements
other than provided for Ordinary Hazard Group II in NFPA #13; the
system
could be inadequate and will not be in compliance with code.

If you or your tenants have specific questions we will be glad to
assist in
any way that we can.

(Best I can do on a Friday afternoon.)

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Friday, August 03, 2007 3:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Owner's Information Certificate

Greg - sounds like you are handling it very professionally (well, ok,
except
for the fuming part) with your letter which will complement the data
nameplate on the riser.  I'd try and avoid the negatives in the letter
and
maybe state the various types of occupancies for which the system is
properly designed.

Garth

- Original Message -
From: Greg McGahan [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Friday, August 03, 2007 1:39 PM
Subject: Owner's Information Certificate


  New spec warehouse designed for Ordinary Hazard Group II occupancy.
Halfway
  through construction we find out that half of the warehouse is
leased to
a
  major retailer who also performs home improvements and they intend
to
store
  home improvement items in the space.
 
  I thought we were correct in sending the GC an OIC and asking the
tenant
to
  complete and return. It comes back with vinyl siding stored in racks
to
  11'-0.
 
  We inform the owner and GC (one and the same) that the system is
inadequate
  and needs to be addressed. Mr Owner calls me, blesses me thoroughly
for
  trying to monitor the world and asks if I intend to do daily
inspections
of
  the premises to make sure the tenant is storing in accordance with
OH2
and
  etc, etc, etc.
 
  I review 13 4.3 and A4.3 and realize that there is a tremendous hole
in
the
  standard. Although the intent is spelled out in the appendix it
stops
short
  of describing the exact situation that we have here.
 
  Why doesn't it say that the OIC must be reviewed and resigned by the
owner
  after the building is built? In this case the owner feels that if we
have
an
  OIC prior to starting the job we should shut up and move since 13
does
not
  REQUIRE us to revisit the design after that. The change of occupancy
does
  not technically apply since the building has not yet, nor will be
occupied
  when we finish.
 
  In order to cover us, we are going to write a letter stating that
the
system
  is OH2 and any tenants should comply with all that entails or they
are
not
  in compliance and the system is not adequate.
 
  And before you all attack me and tell me to walk, this happens to be
one
of
  the most stable and established GC's in our little town and we
really do
not
  want to alienate him.
 
  Still fuming,
  Greg
 
  Living Water Fire Protection, LLC
  1160 McKenzie Road
  Cantonment, FL 32533
  850-937-1850
  Fax: 850-937-1852
 
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
to:[EMAIL PROTECTED]
  (Put the word unsubscribe in the subject field)
 


___

RE: Telling an AHJ No ?

2007-08-01 Thread Paul Pinigis
We have an AHJ here who has been elevated to deity status by every
spineless architect, engineer, and owner that bends to his every whim
and wish.  He is generally very knowledgeable, but not always correct,
and does not appreciate having his knowledge questioned.  He refused to
even look at a formal interpretation from the ICC because he, don't
know where those people get their ideas.!  He is an AHJ for state-owned
or state-controlled properties and has cost taxpayers many millions of
dollars for things like student computer centers designed to OH2 because
computers have plastic cases, hazardous exhaust systems for rooms where
ounces of cleaning agents will be used, and a multitude of other
requirements.   

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Wednesday, August 01, 2007 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Telling an AHJ No ?

I note from this thread and many others on the subject of what to do
when
the AHJ requires things that are beyond their authority, along with a
telecon I had earlier this week, that it happens far more often than it
should, and there's a wide variance on how we sprinkler guys handle it.

We're all aware that staying current on the codes- NFPA and Building- is
more than a full-time job, and most would agree that a large part of the
membership benefit of AFSA and other associations is assistance in
keeping
up with those changes, advance notice of what's in the pipeline, and
naturally, the AFSA's Informal Interpretations. If it is difficult for
us to
stay atop of just the  FP part of this, and the AHJs we deal with often
lack
our breadth of experience, intimate code knowledge, and they often have
handicap and egress requirements upon which they also must remain
current-
so it is not a surprise that we're often saddled with sorting out valid
corrections from hearsay learned in a seminar and misapplied.

Compounding this is the tenuous adversarial positions we may end up in
if we
tell the AHJ he's wrong, and/or stand up for the rights of the Owner
and/or
our own. We must deal with this guy whenever we're in his jurisdiction,
and
there's no end to the things an AHJ can do to make our lives difficult.
So
many of us simply roll over and if its not a lot of money, we give in.
While
this avoids continuation of a problem on the first job, where schedule
demands may point to rolling over since no time exists to fight, it
sets a
dangerous precedent that the AHJ will expect you to follow in the
future. 

In one jurisdiction, we were asked when we were planning on doing our
bucket test on a 13R installation. I pointed out that this was a 13D
requirement stemming from the possible need to verify the calc-light
option in 13D, but that the calcs run for 13R met a higher standard of
care
and therefore the code doesn't require a bucket test in 13R. He replied
our
competitors all do it. And I responded that that's their option, I'd
rather
educate you on what you're asking for- and he said if its not a
requirement
of 13R, you don't need to do it. So we saved some labor hours on each
job
there, and I trust our competitors no longer have to do it either (at
least
those that bother to read this!). But there was no argument, no lines
drawn
in the sand, just an explanation of where and what the requirement was,
and
why it didn't apply where he was trying to apply it. This was made far
easier from the AHJ's recognition of his own limited knowledge, and his
familiarity with my code knowledge- exhibited in the explanation of not
only
what the code said, but explaining why.

The larger problems arise when we encounter what many of us refer to as
the
badge-heavy AHJ who believes he's been anointed from on high, and
therefore his proclamations are supreme. Having encountered some of
these, I
can understand a second type of response to the AHJ asking for more than
he's entitled to- dump it in the Owner (or GC's) lap and ask if they
want to
fight or give it to him. I don't want to know how much money has been
wasted
on pacifying the clueless. This doesn't end the war, it just lets him
win
the battle and have precedent set that he gets his own way, when he
really
needs to have someone explain what local amendments are, how they are
obtained, and without them, you have the base building code.

The more we cave in to excessive demands, the longer the problem will
persist.

glc




-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, August 01, 2007 12:22 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Check valve in 13D system

I second Ron's thoughts. Guys, I cite chapter and verse. You may not
like
reading it or worse doing it but hey its in the code. I'll entertain a
variation if you have a better mousetrap but you gotta do the homework.
Its
pretty simple.

Have the inspector cite it.

John Drucker (AHJ)



RE: Interpretation of nfpa 13, 8.1.1(1)

2007-08-01 Thread Paul Pinigis
If there is nothing on the building code side driving you to have a
sprinklered building, the protecting specific hazards is acceptable, but
you will still not have a sprinklered building.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 12:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

We have met and satisfied all the requirements of the building code for
the installation.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, August 01, 2007 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

Are there allowances for height, area, fire-endurance, etc. being
applied to the project based upon it being sprinklered?  If so, look at
those exceptions very carefully.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 11:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Interpretation of nfpa 13, 8.1.1(1)

I've got a gypsum board mfg. facility.  Several areas are unsprinkled as
permitted by the IFB due to the lack of hazard present and building
separations.  I also have hazardous storage, paper storage and offices
which are sprinkled, again in accordance with the IFB and IFC.  The AHJ
is saying that if we sprinkler anything then EVERYTHING needs to be
sprinkled regardless of what the building code says based on 8.1.1(1).
Sprinklers shall be installed throughout the premises.

Does anyone have a formal interpretation on this sentence?  

If he has his way I'd have to protect 500,000 sf of finished gypboard.  


Craig L. Prahl, CET


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Interpretation of nfpa 13, 8.1.1(1)

2007-08-01 Thread Paul Pinigis
Sweet!

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 1:35 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

Well thanks to those who replied.  We just got a call from the AHJ and
the ruling was changed.   We're good to go.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, August 01, 2007 12:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

If there is nothing on the building code side driving you to have a
sprinklered building, the protecting specific hazards is acceptable, but
you will still not have a sprinklered building.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 12:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

We have met and satisfied all the requirements of the building code for
the installation.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, August 01, 2007 12:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

Are there allowances for height, area, fire-endurance, etc. being
applied to the project based upon it being sprinklered?  If so, look at
those exceptions very carefully.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 11:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Interpretation of nfpa 13, 8.1.1(1)

I've got a gypsum board mfg. facility.  Several areas are unsprinkled as
permitted by the IFB due to the lack of hazard present and building
separations.  I also have hazardous storage, paper storage and offices
which are sprinkled, again in accordance with the IFB and IFC.  The AHJ
is saying that if we sprinkler anything then EVERYTHING needs to be
sprinkled regardless of what the building code says based on 8.1.1(1).
Sprinklers shall be installed throughout the premises.

Does anyone have a formal interpretation on this sentence?  

If he has his way I'd have to protect 500,000 sf of finished gypboard.  


Craig L. Prahl, CET


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Corps of Engineers Grv'd Cplg Spec

2007-07-31 Thread Paul Pinigis
The client paid for the design, but not the cost of producing multiple
sets of drawings to be sent out to bidders.  The small fee that is
charged is not for the design, but for the paper output.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Key, SET
Sent: Tuesday, July 31, 2007 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

You are right Bob, especially when is a Gov. Job. We are suppose to have
a
clause in our contract that states that if we have to pay for drawings
it
will be an extra to the contract. So cost of work goes up. Gov has
already
paid for it once.


Gregg


 








-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, July 30, 2007 3:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

Ron said,
 Something is very wrong in the building industry.  Very true and
there
has been for many years.  Besides all the little niceties that you
mentioned, my pet peeve is the architect or engineer who has been paid
multi-thousands of dollars to provide the owner with plans and specs and
then turns around and wants the sub to pay him another $50, $150, $300,
or
what ever absurd price to transmit you the drawings.  Anyway my rant,
I'm
done.

Bob knight

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Corps of Engineers Grv'd Cplg Spec

2007-07-31 Thread Paul Pinigis
No, that would be robbery.  Emails are free, CDs are usually free, and
paper is based on the actual printing and delivery costs.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, July 31, 2007 8:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

$200 per sheet for email is for paper output?

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, July 31, 2007 7:44 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

The client paid for the design, but not the cost of producing multiple
sets of drawings to be sent out to bidders.  The small fee that is
charged is not for the design, but for the paper output.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Key, SET
Sent: Tuesday, July 31, 2007 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

You are right Bob, especially when is a Gov. Job. We are suppose to have
a
clause in our contract that states that if we have to pay for drawings
it
will be an extra to the contract. So cost of work goes up. Gov has
already
paid for it once.


Gregg


 








-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, July 30, 2007 3:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Corps of Engineers Grv'd Cplg Spec

Ron said,
 Something is very wrong in the building industry.  Very true and
there
has been for many years.  Besides all the little niceties that you
mentioned, my pet peeve is the architect or engineer who has been paid
multi-thousands of dollars to provide the owner with plans and specs and
then turns around and wants the sub to pay him another $50, $150, $300,
or
what ever absurd price to transmit you the drawings.  Anyway my rant,
I'm
done.

Bob knight

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: 10psi Saftey Factor

2007-07-23 Thread Paul Pinigis
Why?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Sunday, July 22, 2007 1:39 PM
To: sprinklerforum@firesprinkler.org
Subject: 10psi Saftey Factor


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: IDOD Dry pipe systems

2007-07-12 Thread Paul Pinigis
IDOD is just a high-quality galvanized pipe that has a nice alloy layer
of zinc and steel on the surface because the pipe is heated to the same
temperature as the zinc bath before it is dipped.  There is no flaking
of the zinc coating that you get when you roll grove lower quality
pipe (e.g. stuff from China) so it has a better corrosion resistance.

I don't think that there are any listing restrictions.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, July 12, 2007 4:56 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: IDOD Dry pipe systems

We have a project with about 120,000 Sf of dry parking garage, which 
requires the use of IDOD for all branchlines, and Galv mains. We have
never 
used the IDOD product and have the following questions for any of you
that 
have:

What is the preferred head out let?(Side outlet coupling?)(Snap-o-lets 
between?)(other?)

Any specific listing restrictions with this product?

Do you order pre-cuts from the factory or cut your own?

Any other suggestions?


Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: IDOD Dry pipe systems

2007-07-12 Thread Paul Pinigis
IDOD is the product name for a galvanized pipe product.  The IDOD came
from Inside Diameter, Outside Diameter since both surfaces are
galvanized. 

 

Paul J. Pinigis, P.E.

Chief Life Safety Engineer

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, July 12, 2007 5:01 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: IDOD Dry pipe systems

 

Educate the sheltered amongst us.  What is IDOD? 

 

 

Craig L. Prahl, CET

Fire Protection Group

Mechanical Department

CH2MHILL

Lockwood Greene

1500 International Drive

PO Box 491, Spartanburg, SC  29304-0491

Direct - 864.599.4102

Fax - 864.599.8439

[EMAIL PROTECTED]

http://www.lg.com

 

 

-Original Message-

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Thom

McMahon

Sent: Thursday, July 12, 2007 4:56 PM

To: sprinklerforum@firesprinkler.org

Subject: Re: IDOD Dry pipe systems

 

We have a project with about 120,000 Sf of dry parking garage, which

requires the use of IDOD for all branchlines, and Galv mains. We have

never used the IDOD product and have the following questions for any of

you that

have:

 

What is the preferred head out let?(Side outlet coupling?)(Snap-o-lets

between?)(other?)

 

Any specific listing restrictions with this product?

 

Do you order pre-cuts from the factory or cut your own?

 

Any other suggestions?

 

 

Thom McMahon

Firetech, Inc.

2560 Copper Ridge Dr

Steamboat Springs, CO 80488-2136

Tel: 970-879-7952

Fax: 970-879-7926

- Original Message -  

 

___

Sprinklerforum mailing list

Sprinklerforum@firesprinkler.org

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email

to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

___

Sprinklerforum mailing list

Sprinklerforum@firesprinkler.org

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email
to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Sprinkler Success Story

2007-06-28 Thread Paul Pinigis
Dan,

Is this a dry pipe or pre-action system?
Did the pipe happen to be made in China?
Was there any testing for the presence of the microbes associated with
MIC?
What type of sprinklers were these?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 5:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler Success Story

Dear Forum members,

I have got the following situation.

A 4 years old system, grid type, 2 galvanized pipes, K=5.6 pendent
sprinklers, bulb type. 

Suspecting that there is a great deal of clogged heads, we run some
tests:

1.  We subjected a sample to 15 psi pressure and initiated the
bulbs. 
2.  Some of the heads burst.  Some did not. 
3.  One head burst at 14 bars, one at 3.5 bars, one at 1.5 bars. 
4.  In the sprinklers that bust, the cone type plastic plug was
ejected,
but the deposit did not, i.e.:  The actual nozzle was about 1/4 of the
full
sprinkler bore area. 

We tested the water. 

The general solid contents were between 277 and 455 mg/L.  

Ca was between 55 and 82 mg/L, 

Mg 32 to 37 mg/L. 

Cl  25 to 27 mg/L

Na 14 to 17 mg/L

Zn 3 to 6 mg/L

We also tested the deposits within some sprinklers that appeared to be
hard
(resulting in a constricted nozzle). 

In these deposits we found a great deal of Iron and Zinc.  

In the deposit one head we found 4% Ca, 50% iron and  4.4% Zinc,

In another one 10% Ca, 1.5% Iron and 20% Zinc. 

Another one 4.5% Ca, 25% Iron, 8% Zinc. 

All came from the same galvanized system. 

This is all very disturbing information. 

It appears that Zinc and Iron ions migrate to the copper based sprinkler
and
creates hard deposit de-capacitating the sprinkler system. 

I would like to hear from other people experience and source of
information
for similar research. 

After all, under NFPA25 one is not supposed to inspect the condition of
sprinklers by dismounting a sample. 
 
DAN, 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Sprinkler Success Story

2007-06-28 Thread Paul Pinigis
I know of a lot of quality issues with galvanized pipe that is coming
out of China.  Does this happen to be Chinese pipe?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 10:44 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler Success Story

This is a standard wet type system. 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Thursday, June 28, 2007 2:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler Success Story

Dan,

Is this a dry pipe or pre-action system?
Did the pipe happen to be made in China?
Was there any testing for the presence of the microbes associated with
MIC?
What type of sprinklers were these?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Thursday, June 28, 2007 5:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler Success Story

Dear Forum members,

I have got the following situation.

A 4 years old system, grid type, 2 galvanized pipes, K=5.6 pendent
sprinklers, bulb type. 

Suspecting that there is a great deal of clogged heads, we run some
tests:

1.  We subjected a sample to 15 psi pressure and initiated the
bulbs. 
2.  Some of the heads burst.  Some did not. 
3.  One head burst at 14 bars, one at 3.5 bars, one at 1.5 bars. 
4.  In the sprinklers that bust, the cone type plastic plug was
ejected,
but the deposit did not, i.e.:  The actual nozzle was about 1/4 of the
full
sprinkler bore area. 

We tested the water. 

The general solid contents were between 277 and 455 mg/L.  

Ca was between 55 and 82 mg/L, 

Mg 32 to 37 mg/L. 

Cl  25 to 27 mg/L

Na 14 to 17 mg/L

Zn 3 to 6 mg/L

We also tested the deposits within some sprinklers that appeared to be
hard
(resulting in a constricted nozzle). 

In these deposits we found a great deal of Iron and Zinc.  

In the deposit one head we found 4% Ca, 50% iron and  4.4% Zinc,

In another one 10% Ca, 1.5% Iron and 20% Zinc. 

Another one 4.5% Ca, 25% Iron, 8% Zinc. 

All came from the same galvanized system. 

This is all very disturbing information. 

It appears that Zinc and Iron ions migrate to the copper based sprinkler
and
creates hard deposit de-capacitating the sprinkler system. 

I would like to hear from other people experience and source of
information
for similar research. 

After all, under NFPA25 one is not supposed to inspect the condition of
sprinklers by dismounting a sample. 
 
DAN, 

Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__ NOD32 2361 (20070628) Information __

This message was checked by NOD32 antivirus system.
http://www.eset.com


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Gang Drain for Attic Dry System

2007-06-28 Thread Paul Pinigis
Yes, unless you put a drain valve on the end of each branch line to
facilitate drainage of each line individually.  Could be expensive.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, June 28, 2007 10:24 AM
To: sprinklerforum@firesprinkler.org
Subject: Gang Drain for Attic Dry System


This question was just posed to me by my Branch Manager - 

In an attic dry system with each branch line ending in what amounts to a
low?point, if the designer interconnected each branch line to?a 1-inch
gang drain, would that not, in effect, create a gridded dry system?

Ray Hoshall
Service Manager
FIRE TECH SERVICES, INC.


AOL now offers free email to everyone.  Find out more about what's free
from AOL at AOL.com.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Steam Room

2007-06-22 Thread Paul Pinigis
What would be your justification for not protecting that room?  I can
not find anything that would permit omission of sprinklers.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Friday, June 22, 2007 1:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam Room

But the question still is; is there somewhere in the code that states
that
this is how you treat a steamroom. In other words do I have to have that
area covered?


Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, June 22, 2007 1:32 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Steam Room

Actually we use 360'F heads in our sauna's and 286 in steam rooms. Steam
is 
212'F max unless its under pressure, (at a pressure above atmospheric)
which

should never occur in a steam room. The sauna is higher because the 
electrical cut out is usually well over 200'F (As high as 300). We
protect 
both as light haz.. even tho the sauna has un-treated wood thru out, can

have more in the way of combustible lotions oils and towels in contact
with 
the dry heat element, than is usually able to happen in the
non-combustible 
steam room.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message - 
From: Jamie Seidl [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Friday, June 22, 2007 11:24 AM
Subject: RE: Steam Room


I talked with a sauna rep awhile back on this same issue.  They
recommend a 286 deg head.


Jamie Seidl



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Steam Room

2007-06-22 Thread Paul Pinigis
I would suggest asking the engineer for his justification for omitting
the room, in writing.  I doubt that you will get anything. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Friday, June 22, 2007 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam Room

I could not find anything either but the engineer did not think it would
need to be covered. Just trying to cover my bases.

Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, June 22, 2007 2:13 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam Room

What would be your justification for not protecting that room?  I can
not find anything that would permit omission of sprinklers.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Biodiesel mfg

2007-06-14 Thread Paul Pinigis
Biodiesel is vegetable oil, and likely a Class IIIB combustible liquid.  You 
should question the classification considering that the flash point of 
vegetable oil is very high.  The following is from an FM document: The closed 
cup flash point of the tested vegetable oil was 450°F (232°C)

Even if this was an oil-cooking facility the density would only be 0.25 gpm/sf 
over 3,000 sq ft (per FM standard on oil cooking equipment).  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - 
work
Sent: Thursday, June 14, 2007 5:02 PM
To: sprinklerforum@firesprinkler.org
Subject: Biodiesel mfg

I have been asked to look at some criteria for a small (2500 sqft) 
biodiesel processing facility. Someone (I'm not sure who) defined 
this as a Class !B flammable liquid and called for a 0.40 gpm/sqft 
density over the entire building area. While I'm not necessarily 
challenging this, I cannot find anything to verify it. NFPA 13 and 30 
seem to focus more on storage than processing. Has anyone else run 
into this yet?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Test

2007-06-08 Thread Paul Pinigis
Ding.

Paul J. Pinigis, P.E.

Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray
Schmid
Sent: Friday, June 08, 2007 7:08 AM
To: sprinklerforum@firesprinkler.org
Subject: Test

 

 

Ray Schmid, P.E.

Principal

Koffel Associates, Inc.

410-750-2246

www.koffel.com http://www.koffel.com/ 

This communication is confidential. This information may be privileged
and is intended for the exclusive use of the above named addressee(s).
If you are not the intended recipient(s), you are expressly prohibited
from copying, distributing, disseminating, or in any other way using any
of this information contained herein. If you have received this
communication in error, please contact the sender by telephone at (410)
750-2246 or by response via e-mail and then permanently delete the
original email and any copies.

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: FDC check valves

2007-05-31 Thread Paul Pinigis
In my 1983 edition the requirement is listed and there is a bar next to
the section indicating that it was either new or changed.  But, there
are other references to the check valve that don't indicate changes, so
the requirement definitely predates 1983.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Sean 
Christine Conlin
Sent: Thursday, May 31, 2007 9:44 AM
To: sprinklerforum@firesprinkler.org
Subject: FDC check valves

Good day to all!
   
  Does anyone know when NFPA 14 or other NFPA standard first initiated
the requirement for a check valve in the fire department connection?
   
  Thanks for the help in advance.
   
  Sean
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Combustible Construction Stair Ways

2007-05-23 Thread Paul Pinigis
(1) the presence of the gypsum board does not change the construction to
non-combustible.

(2) good question, that one is not clear to me.  My initial response
would be yes, but the requirement is vague.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Shawn
Fenneran
Sent: Wednesday, May 23, 2007 2:42 PM
To: sprinklerforum@firesprinkler.org; Bob Caputo
Subject: Combustible Construction Stair Ways

To all:
I am doing a Project 4 Story Residential building witch is designed per
NFPA
13 and it is being built with Type V Construction. The Stairs are being
sheet rock w/ 1 layer of 5/8 GWB underneath all landings, and all walls
in
the stair. It does state in NFPA 13 8.14.3, Combustible Construction.
Sprinklers shall be installed beneath all stairway of combustible
construction.
(1) Does putting 5/8 GYB Sheet rock underneath the landing makes this a
Non
combustible stair?
(2) If this is considered a combustible stair do we have to put
sprinklers
underneath all landings, not just underneath the entry on each floor,
including underneath the intermediate landing between the floors

Thanks
Shawn Fenneran
CET#105218



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Cycling Systems

2007-05-17 Thread Paul Pinigis
Are you referring to the Viking Firecycle system?  If so, they seem to
be most useful on projects with nervous electrical engineers.  I have
proposed them on data center projects just to get electrical engineers
to stop hyperventilating at the thought of having a sprinkler system
discharge in their space, but we have always settled on wet or
preaction.  The only place that I have seen them used in any volume is
in the cable vaults of telephone central offices and in the electrical
rooms of a large government data center.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brooks,
Bill
Sent: Thursday, May 17, 2007 12:59 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Cycling Systems

Not the two wheeled type that have caused me some aggravation.

Can anyone provide feedback on the usefulness of these systems?  What is
the
ideal application if there is one?

Bill Brooks
Pittsburgh, PA
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Carpet Padding Commodity Classification

2007-05-16 Thread Paul Pinigis
It is an expanded plastic, but you would need to know what materials are
used to be any more specific.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Smith,
Steven D. (CSFD)
Sent: Wednesday, May 16, 2007 11:41 AM
To: AFSA SprinklerFORUM
Subject: Carpet Padding Commodity Classification

Forum members,

I couldn't find anything in the archives regarding this. (I noticed that
the archives are limited to the most recent 6 mos) 

At any rate, how would carpet padding (by itself) be classified? I've
got some thoughts but want to hear from others first. 

Thank you in advance.

Steven Smith, CFPS
Fire Protection Engineer II
Colorado Springs Fire Department
719-385-7362

In Omnia Paratus
Fire Engineering Saves Firefighters Lives


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pockets or just plain Obstructions

2007-05-15 Thread Paul Pinigis
Check your math, but first convert 14 to 1.167'.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Tuesday, May 15, 2007 8:40 AM
To: sprinklerforum@firesprinkler.org
Subject: Pockets or just plain Obstructions

Hello sprinklerforum,

  I have a 2 story butler building where the center area of the 2nd
floor is supported by 14 deep steel beams exposed to the floor below.
The space between the beams are 24'-4 long x 4' Wide and the beams are
14 deep supported at each end by a 16 deep beam. IF I did my math
right that figures to 1362.666 cubic feet in each space. Heads down the
length of each space?  Sidewall head at each end in each space? This is
a light hazard building. The space under these beams will be a game room
for a Youth Christian Center. I am open to suggestions to protect this
area AND keep the pool cues away from the sprinkler heads..

-- 
Best regards,
Charles Thurston 
Coastal Fire Protection
mailto:[EMAIL PROTECTED]


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Re[2]: Pockets or just plain Obstructions

2007-05-15 Thread Paul Pinigis
So what you really have is just simple obstructed construction.  Place
the deflector 1 below the bottom flange of the beam and space them
normally. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Tuesday, May 15, 2007 9:57 AM
To: Paul Pinigis
Subject: Re[2]: Pockets or just plain Obstructions

Hello Paul,

Got my coffee and construction calculator working now and it looks
like 113.5556 cubic feet

Tuesday, May 15, 2007, 8:44:52 AM, you wrote:

 Check your math, but first convert 14 to 1.167'.

 Paul J. Pinigis, P.E.
 Chief Life Safety Engineer

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Coastal
 Sent: Tuesday, May 15, 2007 8:40 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pockets or just plain Obstructions

 Hello sprinklerforum,

   I have a 2 story butler building where the center area of the 2nd
 floor is supported by 14 deep steel beams exposed to the floor below.
 The space between the beams are 24'-4 long x 4' Wide and the beams
are
 14 deep supported at each end by a 16 deep beam. IF I did my math
 right that figures to 1362.666 cubic feet in each space. Heads down
the
 length of each space?  Sidewall head at each end in each space? This
is
 a light hazard building. The space under these beams will be a game
room
 for a Youth Christian Center. I am open to suggestions to protect this
 area AND keep the pool cues away from the sprinkler heads..




-- 
Best regards,
 Charlesmailto:[EMAIL PROTECTED]

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Article on Sprinkler Recall

2007-05-08 Thread Paul Pinigis
Really?!?!?  I am actually a very nice person. I despise lawyers, but
that doesn't make me a bad person.   

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Peter
Nadhazy
Sent: Tuesday, May 08, 2007 7:23 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Article on Sprinkler Recall

Paul pinginis is one of those I wouldn't like to meet in the darkness.
That is all!

--Original Message--
From: Todd Williams - work
Sender: [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
ReplyTo: sprinklerforum@firesprinkler.org
Sent: May 4, 2007 11:05 AM
Subject: RE: Article on Sprinkler Recall

Another purveyor of methinks. I always liked that word (and it's in 
my Spell Check).

At 11:07 AM 5/4/2007, you wrote:
Well, my dad was a corporate patent attorney, not salivating over much
except getting a round of golf below 85 on Saturday. Methinks
Shakespeare is
taken out of context too often; I wouldn't be here otherwise.

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, May 04, 2007 10:45 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

This is America, you can be sued by anyone for anything as long as
there
are scum-bag lawyers salivating at the prospect of making a dollar.  We
should have followed Shakespeare's advice and killed all of the
lawyers.


Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Friday, May 04, 2007 10:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

Could you also be sued by a property owner by calling in enforcement
when
you're not legally obligated to?

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Friday, M

Peter Nadhazy
485 Pine Street
Seekonk, MA 02771
(508)761-4695  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Margarine

2007-05-07 Thread Paul Pinigis
I would suggest storing the margarine with huge amounts of popping corn.
It may not control the fire, but it would be mighty tasty.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Monday, May 07, 2007 1:09 PM
To: sprinklerforum@firesprinkler.org
Subject: Margarine


The NFPA classification of margarine in storage is Class III if oil
content
is below 50% and Class A if between 50% to 80%, all regardless of
packaging.


Anybody knows if this is based on actual testing? 

Is ESFR suitable for this type of storage? 

In the catastrophic fire in Mont Blank tunnel fire a truck carrying
margarine and flour got ignited.  It was found later that in terms of
HRR is
would be similar to gasoline tanker (90% of). 

I would appreciate any info.  


Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Article on Sprinkler Recall

2007-05-04 Thread Paul Pinigis
This is America, you can be sued by anyone for anything as long as there
are scum-bag lawyers salivating at the prospect of making a dollar.  We
should have followed Shakespeare's advice and killed all of the lawyers.


Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Friday, May 04, 2007 10:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

Could you also be sued by a property owner by calling in enforcement
when
you're not legally obligated to?

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Friday, May 04, 2007 7:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

But lets face it a letter to the government AHJ does more then simply
notify someone. This notification unlike any other will result in the
responsible party being compelled to resolve the issue, which
mitigates
the hazard, which reduces the chance of litigation, which protects
property,
which saves lives !

Check with your attorney ask him/her if that makes sense, ask him/her if
a
reasonable person would consider it prudent to notify the authority of
jurisdiction responsible for public safety whenever a condition arose
that
could endanger that safety. 

If uncommon sense doesn't compel someone we have the Fire Codes
reporting
and notification requirements and the legal doctrines of ones duty of
care
and duty to act.

Yours in Fire Safety

John Drucker


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: Thursday, May 03, 2007 11:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

George,

I would think that any professional, be it contractor, designer or 
whatever, who does not notify someone,(I opt for the owner, because 
they have a certain responsibility) of a dangerous condition they are 
aware of, could bear some responsibility if that condition leads to a 
loss. It may be criminal or civil, but the issue remains. I tend to 
equate them because they both involve something I don't like to 
dogive lawyers money. A letter to a building owner, which should 
take no more than 10 minutes to write, could save a lot of headaches 
down the road. Well worth the investment, IMHO.


At 12:45 PM 5/3/2007, you wrote:
While I'll certainly agree it's the right thing to do, I vehemently
disagree
that the sprinkler industry- at least we dumb installing contractors-
have
a
legal or fiduciary duty to contact a fire official.

I believe there is a higher standard for registered design
professionals;
but we work for the building owner in many cases, but we are in no way,
shape or form obligated by any law I'm aware of to act as an
enforcement
entity, or snitch.

That's NOT to say that a widow's lawyer wouldn't drag us in and state
that
we should have recognized a clear and present danger, and taken action-
I
just never heard of any legal requirement.

Has anyone else heard of such a requirement, or case law (outside
Calif)
where a contractor was liable for not contacting an enforcement agency?

Can you imagine an auto mechanic being charged with contributing to
manslaughter if someone drove in, asked him to check their brakes, he
discovers they are defective, the car owner refuses to allow him to fix
them, and drives off- and the mechanic doesn't call the police and give
licenses number, let alone follow in pursuit so as to be able to guide
the
police to the escaping vehicle? If this were the case, there would be
standards requiring mechanics be located in areas with cel reception,
have
cel phones with charged batteries at the ready, and a pursuit vehicle
parked
so as to allow ready exit to pursue.

Anyone aware of a parallel in sprinkler contracting?

George Church
Rowe Sprinkler

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, May 03, 2007 11:23 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall

Todd,

Its really quite simple. Notify your local fire official (AHJ) in
writing of any known fire sprinkler systems where the replacement of
sprinkler heads effected by the recall has not been accomplished. The
sprinkler industry has a duty of care and fire officials have a duty to
act.

Besides all that it's the right thing to do. The last thing the
sprinkler industry needs is a fire loss due to defective product where
the integrity of the industry and fire sprinkler systems in general is
brought into question. Lets seize this opportunity before it slips
away.

Yours in fire safety

John Drucker


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Wednesday, May 02, 2007 8:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Article on Sprinkler Recall


RE: Manual wet standpipes

2007-04-10 Thread Paul Pinigis
If there is city water available, include it too. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Tuesday, April 10, 2007 11:23 AM
To: SprinklerFORUM
Subject: Manual wet standpipes

We have a discussion in our office on the correct way to calculate a
manual wet standpipe.
Our local fire department pumper trucks are set for 150PSI @ 1500 GPM
and contain a 1500 gallon tank  For calculating a manual wet standpipe
back to the fire department connection, should we only use the rated
capacity of the pumper truck or are we allowed to add in the city water
pressure/flow available at the hydrant at which they hook up to?  IE:
Either treat it as a stand alone fire pump off a tank or as a standard
fire pump w/ city water supply added in.   
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Roof Deck

2007-04-09 Thread Paul Pinigis
I should have studied!  I failed!  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis
Mack
Sent: Monday, April 09, 2007 2:03 PM
To: sprinklerforum@firesprinkler.org
Subject: Roof Deck

Ok..this may be a stupid question, but here goes:

If I have concrete tee construction, what can I use as the roof deck.  I
have an area with 28' to bottom of deck and 26'-2 to bottom of tee.  If
I
can use the bottom of tee as the maximum ceiling height, then I can use
0.60
gpm  density using Tyco k17-231 sprinklers.  If I need to use 28', then
the
density goes to 0.80 gpm / sq ft.  This is a retrofit, and the existing
system works with 0.60, but does not work with 0.80.  I am looking for
something to justify the 0.60 gpm as being adequate.

Travis Mack, SET 
MFP Design, LLC
480-505-9271
[EMAIL PROTECTED]

Examine yourselves to see if your faith is genuine. Test yourselves.
Surely
you know that Jesus Christ is among you; if not, you have failed the
test of
genuine faith.  2 Corinthians 13:5 NLT

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.26/752 - Release Date:
4/8/2007
8:34 PM
 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: C urious

2007-03-30 Thread Paul Pinigis
I would suggest that you ask the AHJ for the section that you are
violating. Are you violating Table 8.3.2.5(a)?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Friday, March 30, 2007 2:33 PM
To: sprinklerforum@firesprinkler.org
Subject: RE:C urious

We have an AHJ saying our center-of-tile recessed 155F sprinkler is too
close to the HVAC supply diffuser in an A.T.C. (less than 2') I am
curious
as to what section or paragraph in NFPA-13, 2002 references this
requirement? I can't find it, maybe one of y'all can hep me?


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet.  Maybe a 10 x 10.5 foot
spacing. 

The approach that you take will differ depending upon the ALL of the
factors associated with the project.  A holistic approach to each
project is needed.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is rookie-ish please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi,  flow of 1090 gpm. What I do now to get me in the ballpark is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss  etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go Any thoughts? Suggestions? Better Ideas? 

 

   Regards,

  Brian Harris
First Defense Fire Protection


   mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax



 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
Ok, with the pressure that you have available, you can pretty much
forget extended coverage sprinklers.  The area per sprinkler that gave
you will require the minimum end-head pressure of 7 psi.  If you have a
cushion, you can increase the area per sprinkler as long as you stay
under the curve.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 9:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I'm looking for a way to take the given information (static, residual,
flow)
for a given job and come up with a head spacing (standard or extended
coverage) that will work.

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet.  Maybe a 10 x 10.5 foot
spacing. 

The approach that you take will differ depending upon the ALL of the
factors associated with the project.  A holistic approach to each
project is needed.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is rookie-ish please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi,  flow of 1090 gpm. What I do now to get me in the ballpark is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss  etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go Any thoughts? Suggestions? Better Ideas? 

 

   Regards,

  Brian Harris
First Defense Fire Protection


   mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax



 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
If your required density is 0.20 gpm/sq. ft., a 5.6 k-factor will
require 21.55 psi minimum for 130 sq. ft.  With the flow data that you
described this may be a waste of precious pressure (say that three times
fast!).

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, March 27, 2007 10:10 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

The smaller the K factor the lower the flow accumulation (based on equal
spacing) and orifices smaller than 1/2 are verboten for OH.

You could always develop a hydraulic pipe schedule using different EHP's
to get an idea of the impact on pipe size. You wouldn't want to burn a
lot of the available pressure on the end head and then have a 6 riser.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 7:06 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Ron,
What did you use to come up with 5.6k heads?

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, March 27, 2007 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I think your 40% overage is way too high based on the flow test. A good
design oops, layout will limit the overage to less than 20%. Your not
going to use 20 x 20 EC's because of the flow test and the smaller the K
factor the lower the accumlation in the system so I would recommend 1/2
5.6K heads at 130 max.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 5:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a year so if any thing I ask is rookie-ish please keep that in
mind. I'm looking for ideas that some of you may use when starting a new
project when it comes to selecting what heads (head spacing) to use. For
example: I am starting a retail store (mercantile) that has a Static of
47 psi Residual of
42 psi,  flow of 1090 gpm. What I do now to get me in the ballpark is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From that psi I take out for the BFP, elevation, 40% (friction loss 
etc) and whatever is left I find a head with an end head pressure that's
slightly under that and away I go Any thoughts? Suggestions? Better
Ideas? 

 

   Regards,

  Brian Harris
First Defense Fire Protection


   mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax



 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
If you have an ECOH with a k-factor of 14 it could be done.  I like that
approach.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 10:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Paul,
I was thinking that based on the test results  .2/1500 x 1.4 + 250 hose
=
670 GPM (45 psi from curve). 45 psi - 5psi for BFP - 5psi fro elevation
(12') 40% (friction  etc) = 17 psi. Why wouldn't 16x16 EC heads work
(13.3
end head pressure)?

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Ok, with the pressure that you have available, you can pretty much
forget extended coverage sprinklers.  The area per sprinkler that gave
you will require the minimum end-head pressure of 7 psi.  If you have a
cushion, you can increase the area per sprinkler as long as you stay
under the curve.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 9:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I'm looking for a way to take the given information (static, residual,
flow)
for a given job and come up with a head spacing (standard or extended
coverage) that will work.

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet.  Maybe a 10 x 10.5 foot
spacing. 

The approach that you take will differ depending upon the ALL of the
factors associated with the project.  A holistic approach to each
project is needed.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is rookie-ish please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi,  flow of 1090 gpm. What I do now to get me in the ballpark is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss  etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go Any thoughts? Suggestions? Better Ideas? 

 

   Regards,

  Brian Harris
First Defense Fire Protection


   mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax



 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
Maybe.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Now that's what I wanted to hear So maybe I ain't crazy...

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

If you have an ECOH with a k-factor of 14 it could be done.  I like that
approach.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 10:13 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Paul,
I was thinking that based on the test results  .2/1500 x 1.4 + 250 hose
=
670 GPM (45 psi from curve). 45 psi - 5psi for BFP - 5psi fro elevation
(12') 40% (friction  etc) = 17 psi. Why wouldn't 16x16 EC heads work
(13.3
end head pressure)?

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

Ok, with the pressure that you have available, you can pretty much
forget extended coverage sprinklers.  The area per sprinkler that gave
you will require the minimum end-head pressure of 7 psi.  If you have a
cushion, you can increase the area per sprinkler as long as you stay
under the curve.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 9:52 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I'm looking for a way to take the given information (static, residual,
flow)
for a given job and come up with a head spacing (standard or extended
coverage) that will work.

   Regards,
  Brian Harris
First Defense Fire Protection
Design Engineer
   [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax

 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Selecting Heads For a New System

I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet.  Maybe a 10 x 10.5 foot
spacing. 

The approach that you take will differ depending upon the ALL of the
factors associated with the project.  A holistic approach to each
project is needed.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is rookie-ish please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi,  flow of 1090 gpm. What I do now to get me in the ballpark is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss  etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go Any thoughts? Suggestions? Better Ideas? 

 

   Regards,

  Brian Harris
First Defense Fire Protection


   mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
   704.948.3506 phone
   704.948.3507 fax



 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list

RE: Seed Corn

2007-03-27 Thread Paul Pinigis
I would simply consider these to be a plastic commodity to start with.
The fire is going to be initially fuelled by the totes without regard to
what is inside them.  The fire is only going to see plastic as the
fire begins to grow. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Tuesday, March 27, 2007 3:26 PM
To: sprinklerforum@firesprinkler.org
Subject: Seed Corn

Seed corn stored in high-density polyethylene totes. The totes are
approximately 5'x5'x5', completely enclosed (with lid) and are stacked 3
high (15 ft total height). My first thought is NFPA 13 (2002) 5.6.2.3
where
if reinforced high-density polyethylene pallets are used, move up 2
commodity classes. These totes have roughly 5 times as much plastic than
a
pallet, so I'm not sure moving up 2 classes would be adequate
protection.
Anyone out there seen any of these?
Any thoughts? 



David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: owners information certificate

2007-03-20 Thread Paul Pinigis
Don't fool yourself into believing that you can escape liability.  His
lawyers will claiming that you are the expert and you knew about their
future plans and still put in an inappropriate system.  Everything
changes after a loss.

Paul Pinigis

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, March 20, 2007 12:03 PM
To: sprinklerforum@firesprinkler.org
Subject: owners information certificate

Part A:

 

What do we (as an industry) do when an owner completes the Owner's
Information Certificate incorrectly to deliberately mislead an AHJ? 

 

Part B:

 

What do we do when they technically tell the truth as in building a
warehouse that has no storage above 12' initially but they have every
intention (because they tell you so) to store PODS 24' high after they
get a
CO?

 

BTW, the reason I have been unsuccessful in convincing the owner of the
proper level of protection is because there have 2 of these buildings
built
within 200 miles in the last few months and both of them had minimal
systems. The installing contractor on one of the jobs told me that they
were
told the building was a spec warehouse and to protect it as an empty
building and after they were done the owner would lease it to the PODS
franchisee. His comment was I don't know if that protects me or not

 

Legally?

 

Morally I feel bound to walk away from this project but that just means
that
they will find someone else to do the job incorrectly and although there
is
no liability involved, there is still the knowledge that the building
(Ord.
Group II) will be grossly under protected.

 

I know the argument that we are not police of the industry nor can we
2nd
guess what the potential future occupancy of a building is or may be one
day, but this is different and one of the 2 scenarios listed above is
going
to happen on this project.

 

Thanks for your input,

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: owners information certificate

2007-03-20 Thread Paul Pinigis
The difference is in what you know at the time of the sale.  

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Tuesday, March 20, 2007 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: owners information certificate

I sell cars.
Family of 4 walks in, wants ot buy an F150 2 door, no backseat.
I throw them out on their ear since I KNOW they will be strapping the
baby
in the middle seat belt and there's no belt left for the 12 year old.

I feel so used. What if the husband had come in alone? I might have sold
them a means of breaking the law, albeit inadvertently.

I feel better now, their family is now safe.

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 20, 2007 12:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: owners information certificate

Don't fool yourself into believing that you can escape liability.  His
lawyers will claiming that you are the expert and you knew about their
future plans and still put in an inappropriate system.  Everything
changes after a loss.

Paul Pinigis

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, March 20, 2007 12:03 PM
To: sprinklerforum@firesprinkler.org
Subject: owners information certificate

Part A:

 

What do we (as an industry) do when an owner completes the Owner's
Information Certificate incorrectly to deliberately mislead an AHJ? 

 

Part B:

 

What do we do when they technically tell the truth as in building a
warehouse that has no storage above 12' initially but they have every
intention (because they tell you so) to store PODS 24' high after they
get a
CO?

 

BTW, the reason I have been unsuccessful in convincing the owner of the
proper level of protection is because there have 2 of these buildings
built
within 200 miles in the last few months and both of them had minimal
systems. The installing contractor on one of the jobs told me that they
were
told the building was a spec warehouse and to protect it as an empty
building and after they were done the owner would lease it to the PODS
franchisee. His comment was I don't know if that protects me or not

 

Legally?

 

Morally I feel bound to walk away from this project but that just means
that
they will find someone else to do the job incorrectly and although there
is
no liability involved, there is still the knowledge that the building
(Ord.
Group II) will be grossly under protected.

 

I know the argument that we are not police of the industry nor can we
2nd
guess what the potential future occupancy of a building is or may be one
day, but this is different and one of the 2 scenarios listed above is
going
to happen on this project.

 

Thanks for your input,

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Fill times

2007-03-20 Thread Paul Pinigis
(Volume of the pipe) / (pumper truck pump rate in GPM) = time in
minutes.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Tuesday, March 20, 2007 3:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Fill times

Does anyone know where I can find information on how to calculate fill
times
on an exterior dry manual standpipe?
It's installed along elevated roadways and bridges and will be filled by
a
pumper truck.

Thanks,

Tom Duross
FGOL


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum