That data sheet is 13 years old. Does that all still apply today?
-Kyle M
From: José Gregorio Prada Rodriguez
Sent: Thursday, May 9, 2024 7:29 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [External][Sprinklerforum] Re: ESFR Sprinklers and Antifreeze
Agreed; just include that underground in your calculations.
-Kyle M
From: Skyler Bilbo
Sent: Monday, May 6, 2024 2:20 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [External][Sprinklerforum] Re: Water Supply
Bob,
Based on the information you provided, if it
I’d love for someone to explain a little more about how this works. It doesn’t
make sense to me that water would “circulate back” to the truck through the
hoses. All the hoses are on the discharge side of the pumper truck’s pump,
right?
It seems to me that the more likely scenario is that
I think he meant that the pressure should drop if water flows from the pressure
relief valve, while he is manually opening it. Yes, the pressure should drop at
least a little bit when you are discharging water.
With pressures that high, I assume this is a system with a fire pump and jockey
standard in place, then it’s generally
allowed to invoke the “Equivalency” section… i.e. “nothing in this standard is
intended to prevent the use of… methods… of equivalent or superior quality.”
Kyle Montgomery
[cid:image001.png@01DA486D.E07351A0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave
utilize a pilot-operated
pressure-regulating valve at every hose valve location to keep the pressure
right at 100 psi over a wide range of flow, but that would be unorthodox to say
the least.]
Kyle Montgomery
[cid:image001.png@01DA0CDF.597AA0A0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave
If I’m understanding these sections correctly, the occupancy above only really
makes a difference for porte-cocheres (9.2.3.2.1).
Otherwise, I think the need for sprinkler protection or not is determined by
construction type (combustible vs non-combustible), presence/storage of
combustibles,
But, (and I’m deliberately being the devil’s advocate here), which is worse:
1. 10 individual valves controlling small areas, any one of which could be
closed when it shouldn’t be?
2. 1 valve controlling the entire area, but which has to be shut each time
work is done in any of the 10
Reason B gave me a nice hearty chuckle.
-Kyle M
From: Steve Leyton
Sent: Wednesday, August 9, 2023 2:36 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL] [Sprinklerforum] Re: Non-fire connections
We're pretty it's not Kosher because A) it don't seem
Is the whole sprinkler system in the cool area?
Or is there a ceiling with drops down to sprinklers into the cooler and the
branch lines above in the warm area? If that is the case, then it makes sense
that the drops would be colder than the surrounding air and would have
condensation issues.
You measure from the centerline of the offending elbow (the one in the
direction you aren’t allowed to go) to the pump suction flange and you need
those 10 pipe diameters, but you can go up or down as many times as you want to
get the required length, as long as all the elbows you are measuring
I agree with Eric's "something is better than nothing" approach, as long as the
customer/AHJ/etc. understand the limitations of what is being provided. If the
early notification and cooling effect can combine to stop the fire from
spreading to the rest of the house, then that definitely has
Having lived in the desert my entire life, I have no experience with radiant
heat flooring. How hot does it actually get? Even though Bob makes a good point
about heat transfer, I’m not sure the temperature would be high enough to worry
about.
Although, if you can’t drill into the floor, then
It just looks like a bullhead tee. It looks bulbous like that when the outlet
on the tee is a lot larger than the outlets on the run.
-Kyle M
-Original Message-
From: AKS-Gmail-IMAP
Sent: Friday, June 9, 2023 4:14 PM
To: Discussion list on issues relating to automatic fire sprinklers
Negative. It can still be connected to the fire pump and be a manual wet
standpipe. It only becomes an automatic standpipe if/when the fire pump and
water supply is sufficient for the standpipe to operate properly without the
fire department providing flow/pressure through the FDC.
And,
Yeah, the 12" armover limit goes away when using flexible sprinkler
connections. It's in the code:
NFPA 13, 2022 Edition: 17.4.3.4.4.4 "Unless flexible hose fittings... are
used..."
Actually, now that I read that, it just says that you aren't required to use
hangers that restrain the pipe
What I think you should do is adjust/select the PRV to provide a maximum static
outlet pressure of 175-psi based on whatever the maximum static inlet pressure
is. See the Zurn static pressure chart.
This is correct. Setting should be based on maximum static condition.
Then use the 250-gpm flow
What if there was a check valve separating the wet from the dry, and the FDC
was connected to the dry side?
-Kyle M
From: Craig Hanson
Sent: Wednesday, April 5, 2023 7:15 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL] [Sprinklerforum] Re:
We use those remote fuel fill station fairly often because there are a few
jurisdictions nearby that require it. Pryco is one company that makes them. But
they are pretty expensive, so I’m not necessarily suggesting that it’s a good
alternative.
-Kyle M
From: Jason Moore
Sent: Wednesday,
I bet with 80% confidence that there are more unwanted activations in areas
protected by 'Dirty Agents'
than there are fire saves' by 'Dirty Agent' fire suppression systems.
Probably true of water-based fire suppression too though, right?
-Kyle M
From: å...
Sent: Tuesday, March 28, 2023
Yeah, trapeze between two purlins. And maybe put the hangers closer together
than normal to keep the point loads lower.
When we work on PEMBs, there is usually a selection of approved hanger details
included with the structural drawings. Often, they’ll give you maximum weight
loads allowable
I’m pretty sure those initials after your name mean that you can intelligently
evaluate the scenario and suggest an appropriate solution.
-Kyle M
From: Fpdcdesign
Sent: Friday, January 13, 2023 10:26 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL]
I'm not aware of one. But please allow me to officially chortle at the fact
that this guy has got a unit heater hanging in his glass room and he's
concerned about the looks of a pendent sprinkler.
-Kyle M
From: Matt Grise
Sent: Wednesday, December 28, 2022 8:48 AM
To: Discussion list on
room is required?
I realize many jurisdictions might have their own amendments and/or
interpretations, but I'm just wondering from a national code standpoint what
the driving factors are.
Thanks.
Kyle Montgomery
[cid:image001.png@01D915FA.742B6AB0]
Aero Automatic Sprinkler Co.
21605 N. Central
Thank you guys. That answers it.
From: J H
Sent: Monday, December 12, 2022 9:02 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL] [Sprinklerforum] Re: Hydraulic Calculations for CPVC - Tees
- Straight-through Flow
A little more clarification to
NFPA 13 clearly states that "fitting loss for straight-through flow in a tee or
cross shall not be included". But some of the manufacturer's data for CPVC
products specifically lists equivalent lengths for these fittings (tee on the
run) as well as for couplings.
So, are those equivalent
I second this, and this is really your only good option. There’s a reason that
they added the language/section to the new edition.
-Kyle M
From: Matt Grise
Sent: Wednesday, November 2, 2022 9:49 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL]
In this scenario, would the FDC be pressurizing the suction side of the fire
pump? You are usually not supposed to do that.
Kyle Montgomery
[cid:image001.png@01D8DD6E.36E83BC0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom
Could you just put a single head below the diffuser, on the side close to the
return grill, and let that head serve as protection under both obstructions? Or
drop a single head with a water shield right between the two?
It looks like the actual area would be small enough to be covered by one
That section would also seem to indicate that using QR would be OK, don’t you
think? So, maybe you can’t go wrong either way in this scenario.
-Kyle M
From: Matthew J Willis
Sent: Tuesday, September 27, 2022 12:05 PM
To: Discussion list on issues relating to automatic fire sprinklers
Let me play Devil’s Advocate here. James says the building is 40 feet high. So
ESFR protection is probably provided via a table that allows rack storage up to
35 feet high (I’m speculating here, but probably accurate).
If the building is 40 feet tall, then the sprinklers are somewhere below
I’m inclined to side with Travis on this one, but both points are valid and it
probably comes down to the AHJ’s discretion/interpretation.
It would be interesting to hear from Tyco (or someone privy to that info) about
why the SR listing for the heads under those conditions (ordinary hazard and
I believe that there may be some options to treat this area as noncombustible,
such as if it were covered with noncombustible or limited-combustible
insulation. There are some nuances to it, though. Also, I believe you could
consider it noncombustible if the plywood were appropriately
I think you could make that argument, but is it worth the effort? How big is
the area?
I did get a little chuckle out of "possible presence of oil on the drive" being
one of the contributors.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of
I don’t disagree with you, and would almost certainly take the same approach if
I were the installing contractor getting some additional requirement forced
upon me at the 11th hour.
But… one must wonder why the AHJ would make such a request/requirement if not
for some perceived need for
I would say that depends on the reason for requiring this configuration. In my
experience, it is typically done to provide a level of redundancy, i.e. keep
the sprinkler system(s) in service if one of the standpipes is out of service.
In this case, I would suggest that you calculate and size
I agree, Larry. But I'm curious if anyone knows if the committee chose to
specifically exclude those types of tires or if, like you're suggesting, they
just neglected to include them. The format of that definition is kind of weird,
but maybe there was a purpose?
-Kyle M
From: Sprinklerforum
the book says and calculate an area with 4 sprinklers flowing on
each of three branch lines? Or, because of this funky arrangement, do you flow
8 heads on one line and 4 on the next? Or can you meet in the middle and flow 6
heads on each of two branch lines?
Kyle Montgomery
[cid:image001.gif
What about one of the “street vendor” type artists with a few dozen cans of
spray paint?
Then again, if it was originally designed for high-piled storage, would you
expect this occupancy to be any more demanding than that?
From: Sprinklerforum
What if it was two levels of ductwork rather than conveyors? Would you protect
in between the upper and lower ducts, based on that logic?
I’m not saying I disagree with protecting under the upper conveyors in this
case. I’m just saying that there are always going to be gray areas in the code,
I was going to ask about the location of the lights as well. I don’t think NFPA
has any allowances, but does anyone know if they’ve done testing specifically
with obstruction over the aisles only? Do obstructions still negatively impact
ESFR protection if the obstruction are not located over
mum unsupported length.
Any thoughts?
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@aerofire.com<mailto:kmontg
When you are sizing a tank for scenarios like this, do you size for minimum
required discharge (assuming all heads in remote area operating) or expected
actual discharge (assuming all heads in remote area operating)?
Since we're working with hypotheticals, let's say you design a system to work
But, to attempt to answer your question: I think if you have entire branch
lines running under these walkways, then I would think you may have to prove at
least an entire branch line (4 heads). Not in addition, maybe, but say calc two
branch lines overhead (8 heads) and one branch line below (4
This doesn't really answer your question, but how big are these branch lines?
I'm surprised to hear that a walkway (for humans, right?) wouldn't be able to
support a 2-1/2" branch line.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis
I think you do, unless somehow your EC heads meet that spacing criteria (which
would be a horribly inefficient use of EC sprinklers). But I'm hoping someone
will disagree with me and have a good answer as to why you don't.
-Kyle M
From: Sprinklerforum
r coverage the minimum distance out from your room that you haven't
met the intention of the rule.
Fellows, please feel free to shoot some holes in my theory.
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580
My interpretation is that if the top of the suspended or floor-mounted
obstruction is more than 18" below the deflector, then you can ignore it for
obstruction purposes in regardless of if it is light or ordinary hazard. If
ordinary hazard, the obstruction MUST be at least 18" below the
I call BS on your last sentence. Either that, or you should be teaching lessons
on that. The exact same system but with a different number of branch lines can
easily move the remote area one head left or right. Are you really that good? ☺
I agree with the first two sentences. Unless it’s really
I declare: BANKRUPTCY
That's legally binding, right?
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Steve Leyton
Sent: Monday, April 8, 2019 4:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Unsubscribe
People of Earth:
If
So, are we in agreement that the code allows wet sprinklers in this situation
(coolers maintained below 40 degrees but above freezing) but that the “safe”
approach is to use dry pendents?
Step 1 for me is to establish (get comfortable with) the fact that NFPA 13
allows this. Step 2 will be
Yeah, once you have to decide between buying 400 pendents or 400 dry pendents,
it’s a little easier to find yourself on the unconservative (non-conservative?
Liberal?)... the side that doesn’t want to spend that much money.
I know that isn’t a popular opinion around here sometimes, but that’s
2019 NFPA 13:
16.4.1.1 Where any portion of a system is subject to freezing AND the
temperatures cannot be reliably maintained at or above 40 degrees F, the system
shall be installed as a dry pipe or preaction system.
I’m sure this has been discussed before, but the above statement requires
e you prohibited
from using ESFR heads?
It seems strange that you wouldn’t be able to use them in that case, since you
would be able to maintain the appropriate deflector distance (up to 18” from
deck is allowable for some ESFRs) and there would be no actual obstruction to
the sprinklers. Is there so
be able to use them in that case, since you
would be able to maintain the appropriate deflector distance (up to 18” from
deck is allowable for some ESFRs) and there would be no actual obstruction to
the sprinklers. Is there something that I am missing?
Kyle Montgomery
[cid:image001.gif@01CAA0CE
No one uses the old Farmer’s Almanac anymore?
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of tston...@comcast.net
Sent: Thursday, March 14, 2019 10:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Antifreeze temperature
What if you connected the outlet to a flow meter (like what you would use to
measure the flow when setting/testing pressure-reducing valves)? If you got
good numbers for flow and pressure at the riser, wouldn’t this be just about
the most accurate way to do it? Since you have actual data at the
Let us know. I'm sorry you're going through this with OSHPD, but it kind of
makes me feel good that I'm not the only one. They can be pretty tough to work
with and stubborn on their interpretations.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Rocci
Yeah, we've had some issues with the cheaper "factory set at 175 psi" versions.
The adjustable ones work pretty well, I think.
In the original poster's case, is there any reason why it would make sense to
set them at anything other than 175 psi?
-Kyle M
From: Sprinklerforum
I’m thinking that “perpendicular” in the code you referenced is intended to
mean perpendicular in plan view, not perpendicular in an elevation (or
3-dimensionally). Like where the walls don’t form 90-degree angles in plan view.
In fact, I would say that the preceding section stating that
round to the other side or is
there an acceptable minimum distance? It seems like overkill to require the
fill line to be 90 feet away from the suction. I mean, if it was a small tank
with a diameter of 20 feet, then only 20 feet away would be acceptable, right?
Any thoughts?
Kyle Montgome
he code section below:
[cid:image002.png@01D4CF44.FC735690]
What is it prohibiting us from doing, if anything?
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@ae
, then only 20 feet away would be acceptable, right?
Any thoughts?
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.
All,
What is the intention of the highlighted wording in the code section below:
[cid:image001.png@01D4CF40.93B9C930]
What is it prohibiting us from doing, if anything?
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
I’ve seen this condition happen pretty regularly. I’m not aware of anything
prohibiting it. I suppose you are concerned about the potential impact to
sprinkler activation?
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Jamie Seidl
Sent:
Craig,
I’m not a registered sprinkler scientist either, but I would say that,
considering these are small private garages, the sprinklers would almost
certainly activate even if only the lower car was burning. Maybe I’m wrong, but
I don’t think there is anywhere for the heat to go. And
Does it have to be one versus the other, or are we really just looking at two
separate but equivalent protection methods? EH2 for ceiling level only –OR- OH2
at the ceiling if you add protection below.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
I wasn’t singling you out, Matt, just saying that’s the thought process of a
lot of people.
And it makes sense, if you’re an Engineer or work for a company that only does
design, it costs no more to draw a 6” main than a 3” main (for example). But it
costs someone about 4 times as much to
I always get a kick out of the “don’t forget, the code is just the MINIMUM”
comments. Like it’s borderline criminal to use the less restrictive code
requirements and that the contractors who do so are some kind of crooks that
have no consideration for the safety of building occupants or first
There is a section in NFPA that tells you when you need to use a return bend
and when you do not. NFPA 13 7.2.2.
I don’t see a reason why it would not be allowed to come directly out the
bottom of a 4” main, if you are otherwise allowed to come directly out the
bottom of a branch line. There
Good luck if you’ve got ESFR sprinklers and they can’t lower the heaters.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Larry Keeping
Sent: Friday, January 11, 2019 8:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Radiant
Wait, are you planning to use the ZW4004 as the control valve, with the hose
valve downstream and no system control valve or check valve? I’m not sure if
you could do that, because then it’s like the hose valve is coming off the
sprinkler system. I don’t see it as a problem from a practical
This is a legit way to do it. You can get that valve with a capped bonnet if
you don’t want to have an extra unnecessary control valve.
Travis is thinking of a pilot-operated pressure reducing valve (pressure
regulating valve?) which is also legitimate, and gives you more residual
pressure to
Sorry to sidetrack the original conversation, but how does being listed for use
with head guards make it any better for institutional use than any other
sprinkler?
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ben Young
Sent: Tuesday,
FYI, In most applications you can hold Control and scroll up on the mouse to
zoom in/increase text size. Just in case others aren’t as accommodating as Scot.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ron Greenman
Sent: Friday, January 4, 2019
Do you have a gauge on the suction side? If so, what does it read when the
jockey is off and when it is running?
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ben Hill
Sent: Wednesday, December 26, 2018 11:34 AM
To:
So, are we saying that he needs sprinklers above the ceilings, but that it is
OK to use standard spray in spaces less than 36” deep?
Maybe I’m misunderstanding, but isn’t one of the main reasons for attic
(combustible concealed space) heads because the standard spray pattern can’t
develop
If money is no object, go to Young Engineering Manufacturing, Inc.
http://youngeng.com/surge-suppressors-bsa-fire/
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mike Hairfield
Sent: Friday, December 14, 2018 6:02 AM
To:
So, in that case, would they be required to eliminate the non-indicating gate
valve? Or just add the PIV? I mean, if the gate valve is closed, it really
doesn’t matter what position the PIV is in.
I know there are some jurisdictions in Nevada where we’ve been required to
provide wall PIVs for
There is actually some sense to this. Not because of the color, but just to
make sure the ordinary temp heads don’t end up in the wrong location.
It’s no fun when you get a call from the fitter as he get near the top of a
high-rise apartment that goes something like this: “I need to order more
Depends on how you read that table (6.2.5.1). The way I read it, says that you
can only use ordinary temp heads if your maximum ceiling temperature is 100
degrees or less.
And you can only use intermediate temperature heads if your maximum ceiling
temperature is 150 degrees or less.
But it
What Steve said.
Generally, my experience has been that if they have a heat pump, max outlet
temperature will be less than 100 degrees. But if they have a furnace, there is
a good chance it will be higher. Mechanical designer/contractor should be able
to answer the question.
-Kyle M
From:
Yes.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mike Hairfield
Sent: Monday, November 5, 2018 10:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Main Relief Valve for Diesel Driven Fire Pump
Has anyone ever installed a main
I would think that QR is OK but that C-Factor should still be reduced (100).
What does the rest of the forum say?
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Bob Knight
Sent: Thursday, November 1, 2018 3:35 PM
To:
See 11.2.3.2.5 and A.11.2.3.2.5.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Kyle.Montgomery
Sent: Thursday, November 1, 2018 3:19 PM
To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Single Preaction
One of the biggest impacts is that calculating as a dry system means you have
to increase remote area size by 30%, but you don't have to do that if you can
calculate as wet.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Bob Knight
Sent:
I still need to verify, but it looks like it’s going to have a
limited-combustible facing that is stapled in place. For the sake of this
argument, let’s assume that is the case. So, it would be most similar to Figure
A.8.15.1.2.17, with the following differences:
1. It’s a steel bar
I'm looking at a building with steel bar joists with a wood nailer and plywood
deck. The building will have a drop ceiling, and of course have pendent
sprinklers protecting the area below the ceiling.
If there is insulation at the deck that covers the deck and wood nailers, do I
need upright
n NFPA
13 outside of the ESFR section. It sure seems like if it's appropriate for ESFR
heads (arguably the most finicky with regard to spacing/obstructions) that the
same spacing should be OK for standard spray sprinklers.
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprink
ng about
taking this to the AHJ to see if they would allow it, but I don't want to
suggest doing it if there is good reason to believe that it is a "bad fire
protection practice".
I appreciate the input.
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkle
ood reason to believe that it is a "bad fire
protection practice".
I appreciate the input.
Kyle Montgomery
[cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@aerofire
for this, but I haven't found anything in NFPA
13 outside of the ESFR section. It sure seems like if it's appropriate for ESFR
heads (arguably the most finicky with regard to spacing/obstructions) that the
same spacing should be OK for standard spray sprinklers.
Kyle Montgomery
[cid:image001
Tolco has the Figure 4LA which goes up to 12” (FM-Approved). It’s basically a
pipe clamp with a built-in attachment to the brace pipe.
To answer your question, I think that the components of the assembly have to be
listed for use as a seismic brace. So I don’t think you can just grab any 10”
Those are pretty expensive though, aren’t they? If you look at the sprinkler
cut sheets from Reliable (and others) they generally list the White Polyester
heads as “corrosion resistant” and we’ve used those. I don’t think the white
polys cost that much more than your standard sprinkler.
We’ve
2) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Kyle Montgomery
Sent: Thursday, September 13, 2018 9:44 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: [EXTERNAL] RE: Sprinkler h
water loss? Less than all the engineering I’ve
proposed.
I get to see the results of piece-meal far too often.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Kyle Montgomery
Sent: Thursday
Pressure relief valves are “conceivably a waste of money”... coming from the
guy that suggested the forensic metallurgist.
How much will the forensic metallurgist charge Larry to tell him it’s time to
replace his 50-plus year old heads?
Sent from my iPhone
On Sep 13, 2018, at 6:02 PM, Scott
Your statement seems to contradict itself. You say that they are essentially
prepared for multiple options, but that we (the fire protection design
community) should be forced to comply with the "flavor of the week" that the
current fire marshal prefers.
As was stated previously, there are
Which code section requires automatic standpipes for detention facilities? How
long has that been in the code?
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Reed A. Roisum, SET
Sent: Wednesday, September 5, 2018 5:38 PM
To:
I see the same language in quite a few places in chapter 17, but I’m looking
specifically at Figure 17.2.1.2.1(f). The criteria is for “storage 25 ft in
height with 5 ft to 10 ft clearance to ceiling”. So that leads me to believe
the ceiling could be up to 35 feet… is that right?
The language