[Sprinklerforum] Re: Seismic bracing requirements in Canada

2022-08-16 Thread Barry Clarke
inklerforum] Seismic bracing requirements in Canada It’s been awful quiet around here lately. I’ve got a project in Saskatchewan Canada. Industrial facility. Structural engineers can’t tell me if seismic bracing is required or not. After reading through the Canadian Building and Fire code

Re: Seismic Bracing

2017-03-21 Thread Parsley Consulting
te: Rocci, You're correct in one way, the '16 edition no longer allows the use of hanger rods less than 6" long to omit lateral seismic bracing on mains, if the Cp value is greater than 0.50. That does indeed cover most of California, and several other places

Re: Seismic Bracing

2017-03-20 Thread Travis Mack
;> Rocci, >> You're correct in one way, the '16 edition no longer allows the use of >> hanger rods less than 6" long to omit lateral seismic bracing on mains, if >> the Cp value is greater than 0.50. That does indeed cover most of >> California, an

Re: Seismic Bracing

2017-03-20 Thread rongreenman .
7;16 edition no longer allows the use > of hanger rods less than 6" long to omit lateral seismic bracing on mains, > if the Cp value is greater than 0.50. That does indeed cover most of > California, and several other places as well. > That change was added to 9.3.5.5.10.2, (4) in th

Re: Seismic Bracing

2017-03-20 Thread Parsley Consulting
Rocci, You're correct in one way, the '16 edition no longer allows the use of hanger rods less than 6" long to omit lateral seismic bracing on mains, if the Cp value is greater than 0.50. That does indeed cover most of California, and several other places as well.

RE: Seismic Bracing

2017-03-20 Thread Rocci Cetani 3
erforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Monday, March 20, 2017 12:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Seismic Bracing Short rods only eliminate lateral bracing. You will still need longitudinal bracing. Travis Mack, SET MFP Design

Re: Seismic Bracing

2017-03-20 Thread Travis Mack, SET
Short rods only eliminate lateral bracing. You will still need longitudinal bracing. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/9221841

Seismic Bracing

2017-03-20 Thread Tony Silva
In a 13R building there are a 2" cpvc blazemaster supply mains run to supply the upper floor sprinkler systems. The piping will be supported using 2" long rods. The location requires seismic protection. Will sway bracing be required? Any other requirements? Thanks, Tony __

Re: Seismic bracing clips

2015-12-31 Thread Roland Huggins
Exactly what 5 yr inspection are you referring to? NFPA 25 inspections do NOT look at ANY installation issues. Have your contractor provide explicit references to requirements from the standard in place when the system was installed (as Scot already flagged). Roland Huggins, PE - VP Enginee

Seismic bracing clips

2015-12-31 Thread å . . . . . . .
Larry: Seismic bracing requirements have tightene up a lot since the 1970's for fire sprinklers. Bracing was often referred to as the weakest aspect of a sprinkler system prior to the turn of the century. You can probably find a copy of NFPA 13 (Sprinkler Installation Standard) at your

Seismic bracing clips

2015-12-30 Thread Larry Block, Property Manager
Hi, I manage a 1970 vintage concrete tilt-up industrial park with a panelized roof in Southern California. As part of my 5-yr, my contractor is telling me that I need to install seismic clips on some of the locations where the pipes traverse a hanger (v-hangers, in this case). I am looking for i

RE: Seismic Bracing for CPVC

2015-07-16 Thread Steve Leyton
Bracing for CPVC I have a project that requires Seismic bracing. The project is 1", 1-1/4", and 2" CPVC. Recommendations Please? Thank you, Mark E. Eckard SET 1025 Tate Blvd. / P.O. Box9489 Hickory, NC 28602 / 28603 Office: 828-328-6363 Fax: 828-328-6370 Cell: 828-851-0080 Licensed

Seismic Bracing for CPVC

2015-07-16 Thread Mark Eckard
I have a project that requires Seismic bracing. The project is 1", 1-1/4", and 2" CPVC. Recommendations Please? Thank you, Mark E. Eckard SET 1025 Tate Blvd. / P.O. Box9489 Hickory, NC 28602 / 28603 Office: 828-328-6363 Fax: 828-328-6370 Cell: 828-851-0080 Licensed Fire Protec

Re: Seismic bracing design per SDC

2015-05-27 Thread Parsley Consulting
..@ch2m.com wrote: One of the ever hot topics, seismic bracing design. Question is this, for SDC of C it is typical to utilize the design calculations procedures within NFPA 13.I had some other information that stated for a SDC of D that special engineering was required for the seismic brac

Seismic bracing design per SDC

2015-05-27 Thread Craig.Prahl
One of the ever hot topics, seismic bracing design. Question is this, for SDC of C it is typical to utilize the design calculations procedures within NFPA 13.I had some other information that stated for a SDC of D that special engineering was required for the seismic bracing through

Re: Seismic bracing

2014-09-05 Thread Parsley Consulting
:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, September 05, 2014 12:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Since it is an existing building I doubt any of the things you have listed will be done. I gue

Re: Seismic bracing

2014-09-05 Thread Parsley Consulting
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, September 05, 2014 12:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Since it is an existing building I doubt any of the things you have listed

RE: Seismic bracing

2014-09-05 Thread Jim Davidson
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, September 05, 2014 1:46 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Since it is an existing building I doubt any of the things you have listed will be done. I guess I

RE: Seismic bracing

2014-09-05 Thread Cahill, Christopher
014 List of 100 Best Companies to Work For -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, September 05, 2014 12:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing

RE: Seismic bracing

2014-09-05 Thread RFletcher
f Jim Davidson Sent: Friday, September 05, 2014 9:28 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing The seismic design classification should be determined by the structural engineer who determines the SDC of the site. Once the SDC is determined then you can go into e

RE: Seismic bracing - Responsibility (NJ)

2014-09-05 Thread John Drucker - Home
ssage- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jim Davidson Sent: Friday, September 5, 2014 11:43 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Ron, I hope you have a hold harmless letter from the building owner and or develo

Re: Seismic bracing

2014-09-05 Thread ampeck
--Original Message- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of wmens...@comcast.net > Sent: Friday, September 05, 2014 11:58 AM > To: sprinklerforum > Subject: Re: Seismic bracing > > > > Oh boy, here we go again. Eve

RE: Seismic bracing

2014-09-05 Thread Jim Davidson
u for your cooperation. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of wmens...@comcast.net Sent: Friday, September 05, 2014 12:16 PM To: sprinklerforum Subject: Re: Seismic bracing Oh boy, here we go again.  Every time the su

RE: Seismic bracing

2014-09-05 Thread Jack Carlson
forum-boun...@lists.firesprinkler.org] On Behalf Of wmens...@comcast.net Sent: Friday, September 05, 2014 11:58 AM To: sprinklerforum Subject: Re: Seismic bracing Oh boy, here we go again.  Every time the subject of seismic bracing / protection comes up, it shows that there is a general lack of und

RE: Seismic bracing

2014-09-05 Thread RFletcher
ismic bracing Oh boy, here we go again.  Every time the subject of seismic bracing / protection comes up, it shows that there is a general lack of understanding among contractors and designers (myself included) as to when it is required, what is required, and how to do it correctly. We need

RE: Seismic bracing

2014-09-05 Thread RFletcher
-boun...@lists.firesprinkler.org] On Behalf Of Jim Davidson Sent: Friday, September 05, 2014 8:43 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Ron, I hope you have a hold harmless letter from the building owner and or developer because the sprinkler contractor will b

Re: Seismic bracing

2014-09-05 Thread Travis Mack
il:tm...@mfpdesign.com On 9/5/2014 8:58 AM, wmens...@comcast.net wrote: Oh boy, here we go again. Every time the subject of seismic bracing / protection comes up, it shows that there is a general lack of understanding among contractors and designers (myself included) as to when it is required, wh

Re: Seismic bracing

2014-09-05 Thread wmenster
Oh boy, here we go again.  Every time the subject of seismic bracing / protection comes up, it shows that there is a general lack of understanding among contractors and designers (myself included) as to when it is required, what is required, and how to do it correctly. We need more education

Re: Seismic bracing

2014-09-05 Thread Todd - Work
I have never had an AHJ in either CT or MA ask for calcs for seismic bracing. Most just want to see something. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) > On Sep 5, 2014, at 11:10 AM, wrote: > > Some jurisdictions around her

RE: Seismic bracing

2014-09-05 Thread Jim Davidson
ooperation. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, September 05, 2014 11:16 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing Some jurisdictions around here re

RE: Seismic bracing

2014-09-05 Thread RFletcher
t: Friday, September 05, 2014 5:11 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Seismic bracing Stephen, I don't believe the AHJ you're dealing with has thought this decision through very carefully. They seem to be equating "seismic bracing" with "s

RE: Seismic bracing

2014-09-05 Thread Craig.Prahl
e past and have little to no meaning anymore. I can have two buildings 50 ft apart and one require seismic bracing and one not require it. The factors determining that are not difficult to maneuver through but take some knowledge of the Building Code and hazards present, building use, soil

RE: Seismic bracing

2014-09-05 Thread Craig.Prahl
Brooks Sent: Friday, September 05, 2014 10:09 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing "Does anyone know if this is an actual standards requirement or just a preference of the local AHJ ?" One way to do this would be to ask the AHJ. This is something

Re: Seismic bracing

2014-09-05 Thread Parsley Consulting
Stephen, I don't believe the AHJ you're dealing with has thought this decision through very carefully. They seem to be equating "seismic bracing" with "seismic protection", which includes such other features as flexible couplings, clearance requirements,

RE: Seismic bracing

2014-09-05 Thread Bill Brooks
ehalf Of Steve Sorrell Sent: Friday, September 05, 2014 8:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: Seismic bracing I need some help with a seismic problem. I am making modifications to a 1970's sprinkler system in NC, we are using the 2000 ed of NFPA 13. There is no seismic b

RE: Seismic bracing

2014-09-05 Thread Steve Sorrell
nklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing The AHJ can't just "require it". His preference is not relevant. Also seismic bracing is not based on Zones or Maps anymore, hasn't been for quite a while. I'm curious why you're using the 2000 edition of NF

RE: Seismic bracing

2014-09-05 Thread Craig.Prahl
9:11 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Seismic bracing Check the structural notes. If it is seismic design category a or b, then no seismic. If SDC of C or higher then bracing required. It seems odd to do seismic bracing of piping if the building is not designed to resi

Re: Seismic bracing

2014-09-05 Thread Travis Mack
Check the structural notes. If it is seismic design category a or b, then no seismic. If SDC of C or higher then bracing required. It seems odd to do seismic bracing of piping if the building is not designed to resist seismic forces. Travis Mack, SET MFP Design, LLC Sent from my iPhone

RE: Seismic bracing

2014-09-05 Thread Brad Casterline
@lists.firesprinkler.org Subject: RE: Seismic bracing The AHJ can't just "require it". His preference is not relevant. Also seismic bracing is not based on Zones or Maps anymore, hasn't been for quite a while. I'm curious why you're using the 2000 edition of NFPA 13. An

RE: Seismic bracing

2014-09-05 Thread Craig.Prahl
The AHJ can't just "require it". His preference is not relevant. Also seismic bracing is not based on Zones or Maps anymore, hasn't been for quite a while. I'm curious why you're using the 2000 edition of NFPA 13. Anyway back to seismic. Seismic requirements ar

RE: Seismic bracing

2014-09-05 Thread Duane Johnson
nklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Sorrell Sent: Friday, September 05, 2014 8:20 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic bracing The building code requires it. How effective would a partially braced system be, only th

RE: Seismic bracing

2014-09-05 Thread Steve Sorrell
Of Forest Wilson Sent: Friday, September 05, 2014 8:15 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Seismic bracing Does the building code require it? The building code dictates if you are in a seismic zone and NFPA 13 tells you how to do it. On 9/5/2014 8:13 AM, Steve Sorrell

Re: Seismic bracing

2014-09-05 Thread Forest Wilson
g the 2000 ed of NFPA 13. There is no seismic bracing on this system. I have had to add some new main in various areas. The local AHJ is requiring that only the new sprinkler main will need to be braced. Does anyone know if this is an actual standards requirement or just a preference of the loca

Seismic bracing

2014-09-05 Thread Steve Sorrell
I need some help with a seismic problem. I am making modifications to a 1970's sprinkler system in NC, we are using the 2000 ed of NFPA 13. There is no seismic bracing on this system. I have had to add some new main in various areas. The local AHJ is requiring that only the new sprinkler

Re: seismic bracing calcs

2014-02-21 Thread Todd - Work
> > SML > > > > -Original Message- > From: sprinklerforum-boun...@lists.firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > Todd - Work > Sent: Friday, February 21, 2014 2:05 PM > To: sprinklerforum@lists.firesp

Re: seismic bracing calcs

2014-02-21 Thread Charles Thurston
> SML > -Original Message- > From: sprinklerforum-boun...@lists.firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > Todd - Work > Sent: Friday, February 21, 2014 2:05 PM > To: sprinklerforum@lists.firesprinkler.org > Sub

RE: seismic bracing calcs

2014-02-21 Thread Steve Leyton
Behalf Of Todd - Work Sent: Friday, February 21, 2014 2:05 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs Steve, I have seen that list. If you look closely, most of those readings are from the eastern provinces of Canada. There are some in CT, but most are in th

Re: seismic bracing calcs

2014-02-21 Thread Todd - Work
n out on the Pats in the AFC > Championship game. > > Steve > > > > > -Original Message- > From: sprinklerforum-boun...@lists.firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > Todd - Work > Sent: Friday, February 21, 2014 1:21

Re: seismic bracing calcs

2014-02-21 Thread rongreenman .
.@lists.firesprinkler.org] On Behalf Of > Todd - Work > Sent: Friday, February 21, 2014 1:21 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: seismic bracing calcs > > I think you also need to take into account regional differences. Some > areas, like Leytonland, have a

RE: seismic bracing calcs

2014-02-21 Thread Steve Leyton
From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Friday, February 21, 2014 1:21 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs I think you also need to take into account reg

Re: seismic bracing calcs

2014-02-21 Thread Todd - Work
firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve > Leyton > Sent: Friday, February 21, 2014 10:27 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: seismic bracing calcs > > This goes to perpetuate the notion that we're

RE: seismic bracing calcs

2014-02-21 Thread Steve Leyton
ssage- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Friday, February 21, 2014 10:18 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs I think the reason we are s

RE: seismic bracing calcs

2014-02-21 Thread RFletcher
r.org Subject: RE: seismic bracing calcs This goes to perpetuate the notion that we're different or special and that's good and okay. I respectfully disagree - it's not. Every other discipline is required to structurally engineer their supports, coordinate loads and attachme

Re: seismic bracing calcs

2014-02-21 Thread Brad Casterline
.2322 Cell > Skype: steven.scandaliato > > > -Original Message- > From: sprinklerforum-boun...@lists.firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bill > Brooks > Sent: Friday, February 21, 2014 8:14 AM > To: sprinklerforum@list

RE: seismic bracing calcs

2014-02-21 Thread Steven Scandaliato
14 8:14 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs Exactly. Unless your drawing which shows those little criss-cross arrows are accompanied by calculations AND unless your calculations are acceptable to the project structural engineer, then you do not have a comple

RE: seismic bracing calcs

2014-02-21 Thread Steve Leyton
ot an adequate degree of diligence, IMHO Oops, my soapbox just broke. Steve Leyton -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Denhardt Sent: Friday, February 21, 2014 9:12 AM

RE: seismic bracing calcs

2014-02-21 Thread John Denhardt
- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Scandaliato Sent: Thursday, February 20, 2014 5:13 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs Well that's were we are goi

RE: seismic bracing calcs

2014-02-21 Thread Bill Brooks
nkler.org] On Behalf Of rongreenman . Sent: Friday, February 21, 2014 12:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs How do you locate per 13? How do you know what you did will work? How do you know that 1" x 34" brace at 37 degrees to side of a b

Re: seismic bracing calcs

2014-02-21 Thread jgamble
them and the time to install them, ... We should at least do them right. My two cents.  Sent from my Verizon Wireless 4G LTE smartphone Original message From: "rongreenman ." Date:02/20/2014 10:12 PM (GMT-07:00) To: sprinklerforum@lists.firesprinkler.org Subj

Re: seismic bracing calcs

2014-02-21 Thread Aaron Peck
lose its contents to >> anyone. Please send us by fax any message containing deadlines as incoming >> e-mails are not screened for response deadlines. The integrity and security >> of this message cannot be guaranteed on the Internet. >> >> Original message ---

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
ity and security > of this message cannot be guaranteed on the Internet. > > Original message > From: "rongreenman ." > Date:02/20/2014 11:36 AM (GMT-05:00) > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: seismic bracing calcs > > Fro

Re: seismic bracing calcs

2014-02-20 Thread Forest Wilson Fire Sprinkler Contractor
cannot be guaranteed on the Internet. Original message From: "rongreenman ." Date:02/20/2014 11:36 AM (GMT-05:00) To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs From the Piemontesi to the greasy Sicilian, with molte amore. I won

RE: seismic bracing calcs

2014-02-20 Thread RFletcher
-Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, February 20, 2014 3:30 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs I think the standard

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
inkler.org] On Behalf Of Steven > Scandaliato > Sent: Thursday, February 20, 2014 5:13 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: seismic bracing calcs > > Well that's were we are going to disagree...I haven't put tick marks on a > dwg or required them on a dwg s

RE: seismic bracing calcs

2014-02-20 Thread Craig.Prahl
inkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Scandaliato Sent: Thursday, February 20, 2014 5:13 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs Well that's were we are going to disagree...I haven't put tick marks on a d

RE: seismic bracing calcs

2014-02-20 Thread Steve Leyton
From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Scandaliato Sent: Thursday, February 20, 2014 2:13 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs Well that's were we are going to di

Re: seismic bracing calcs

2014-02-20 Thread Steven Scandaliato
pipe size then we got way bigger problems than seismic features... Sent from my BlackBerry 10 smartphone. From: craig.pr...@ch2m.com Sent: Thursday, February 20, 2014 4:04 PM To: sprinklerforum@lists.firesprinkler.org Reply To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing

RE: seismic bracing calcs

2014-02-20 Thread Craig.Prahl
2 craig.pr...@ch2m.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, February 20, 2014 4:33 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing

RE: seismic bracing calcs

2014-02-20 Thread Steve Leyton
t: RE: seismic bracing calcs I have specified the shop drawings and bracing calculations be submitted to the project structural engineer to confirm the adequacy of the attachment point to resist the loading. Is this a common practice? Bill Brooks -Original Message- From: sprinklerforum

RE: seismic bracing calcs

2014-02-20 Thread Bill Brooks
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Thursday, February 20, 2014 4:45 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs And we haven't gotten approval for a document set without including all of those thin

RE: seismic bracing calcs

2014-02-20 Thread Steve Leyton
-boun...@lists.firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, February 20, 2014 11:37 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs Steven, I have never received a contractor shop drawing that covered things to the detail you describe. It'

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
sprinkler.org] On Behalf Of Steven > Scandaliato > Sent: Thursday, February 20, 2014 11:00 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: seismic bracing calcs > > Wait...hold on...just to make sure, and Craig I am sure you probably know > this...BUT we have a

RE: seismic bracing calcs

2014-02-20 Thread Craig.Prahl
sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Scandaliato Sent: Thursday, February 20, 2014 11:00 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs Wait...hold on...just to make sure, and

RE: seismic bracing calcs

2014-02-20 Thread MPhelps
: seismic bracing calcs Since Greenman is pure mongrel (and occasionally junkyard mongrel), apart from being anglicized Gaelic, and the other half is Ferracone. And since I messed up my leg I keep tripping over my fingers, Mr. Noytel. Then there's also the aixelsyd On Thu, Feb 20, 2014 at

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
to:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > Steven Scandaliato > Sent: Thursday, February 20, 2014 8:46 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: seismic bracing calcs > > Hey...you don't want to mess with us...cause god kno

RE: seismic bracing calcs

2014-02-20 Thread Steve Leyton
lf Of Steven Scandaliato Sent: Thursday, February 20, 2014 8:46 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs Hey...you don't want to mess with us...cause god knows...we have "friends"everywhere! Steven Scandaliato, SET CFPS 520.971.2322 Cell Skype

Re: seismic bracing calcs

2014-02-20 Thread IPA
half Of > rongreenman . > Sent: Thursday, February 20, 2014 10:36 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: seismic bracing calcs > > From the Piemontesi to the greasy Sicilian, with molte amore. I won't hold > it against you that your family is from the

RE: seismic bracing calcs

2014-02-20 Thread Steven Scandaliato
nklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, February 20, 2014 10:36 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: seismic bracing calcs >From the Piemontesi to the greasy Sicilian, with molte amore. I won't hold it against you that your family is from the

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
ts.firesprinkler.org] On Behalf Of > Brian Harris > Sent: Thursday, February 20, 2014 6:32 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: seismic bracing calcs > > Both... > > Brian Harris, CET > BVS Systems Inc. > bvssytemsinc.com > > -Original

RE: seismic bracing calcs

2014-02-20 Thread Steve Leyton
arris Sent: Thursday, February 20, 2014 6:32 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: seismic bracing calcs Both... Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum

RE: seismic bracing calcs

2014-02-20 Thread Steven Scandaliato
o, SET CFPS 520.971.2322 Cell Skype: steven.scandaliato -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, February 20, 2014 9:41 AM To: sprinklerforum@lists.firesprinkler.org

Re: seismic bracing calcs

2014-02-20 Thread rongreenman .
rforum-boun...@lists.firesprinkler.org > [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > craig.pr...@ch2m.com > Sent: Thursday, February 20, 2014 7:27 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: seismic bracing calcs > > Seismic design category

RE: seismic bracing calcs

2014-02-20 Thread Cliff Whitfield
fire-design.com www.fire-design.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, February 20, 2014 7:27 AM To: sprinklerforum@lists.firesprinkler.org Subject

Re: seismic bracing calcs

2014-02-20 Thread Travis Mack
There really is no locate per NFPA 13. You still have max of 40/80, 4 way at change in direction and laterals no more than 6' from end of cross main. But, with all of the other requirements in chapter 9, you must calculate the bracing spacing. I consider it just like pipe sizing calcs any more

RE: seismic bracing calcs

2014-02-20 Thread Brian Harris
@lists.firesprinkler.org Subject: seismic bracing calcs Seismic design category C, contractor submittal package, Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 and send typical catalog data sheets? FM Global project, BTW. Craig L. Prahl, CET Fire Protection Group Lead

seismic bracing calcs

2014-02-20 Thread Craig.Prahl
Seismic design category C, contractor submittal package, Do you provide a calc sheet for EQ bracing or just locate per NFPA 13 and send typical catalog data sheets? FM Global project, BTW. Craig L. Prahl, CET Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spart

RE: Seismic Bracing

2014-01-07 Thread Bob
M To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic Bracing Yes, you need a longitudinal brace as Steve said. Lateral braces can act as longitudinal braces if they are within 24 in. of the pipe braced longitudinally and the brace is on a pipe of equal or greater size than the pipe being b

RE: FW: Seismic Bracing

2014-01-07 Thread Brian Harris
Sent: Tuesday, January 07, 2014 2:31 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: FW: Seismic Bracing Brian, There is no option in NFPA 13 which allows omission of longitudinal bracing. In the scenario you describe, the 40' long main would indeed require a longitudinal brace,and an

RE: Seismic Bracing

2014-01-07 Thread Reed A. Roisum, C.E.T.
Steve Leyton Sent: Tuesday, January 07, 2014 1:27 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Seismic Bracing I believe that you need at least one longitudinal brace in the scenario you describe. Steve Leyton -Original Message- From: sprinklerforum-boun

Re: FW: Seismic Bracing

2014-01-07 Thread ParsleyConsulting
Brian, There is no option in NFPA 13 which allows omission of longitudinal bracing. In the scenario you describe, the 40' long main would indeed require a longitudinal brace,and any location along the length of that main would be acceptable, as it must be no more than 40' from the end of the

RE: Seismic Bracing

2014-01-07 Thread Steve Leyton
11:17 AM To: sprinklerforum@lists.firesprinkler.org Subject: FW: Seismic Bracing Is it possible to have a Main that only has Lateral Bracing & no Longitudinal Bracing? Say you have a Main that is 40'-0" long and have a Lateral brace within 6' of each end, are you required to

FW: Seismic Bracing

2014-01-07 Thread Brian Harris
Is it possible to have a Main that only has Lateral Bracing & no Longitudinal Bracing? Say you have a Main that is 40'-0" long and have a Lateral brace within 6' of each end, are you required to have a Longitudinal brace in the middle? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssy

Re: Seismic Bracing - Clean Agent

2011-08-09 Thread Ron Greenman
boun...@firesprinkler.org] On Behalf Of max brown > Sent: Monday, August 08, 2011 6:42 PM > To: burtell > Subject: RE: Seismic Bracing - Clean Agent > > > On our installations we always have additional bracing. Restraint in all > directions similar to underground mains, high pr

RE: Seismic Bracing - Clean Agent

2011-08-09 Thread Rod DiBona
] On Behalf Of max brown Sent: Monday, August 08, 2011 6:42 PM To: burtell Subject: RE: Seismic Bracing - Clean Agent On our installations we always have additional bracing. Restraint in all directions similar to underground mains, high pressure discharge with 360 degree, upward restraint, 180

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread max brown
gt; To: sprinklerforum@firesprinkler.org > Date: Mon, 8 Aug 2011 12:41:01 -0600 > Subject: RE: Seismic Bracing - Clean Agent > > We braced the clean agent as we normally would and interpreted it to mean > that no additional seismic would be required. Sprinkler system in same area &g

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Craig.Prahl
rooks Sent: Monday, August 08, 2011 2:12 PM To: sprinklerforum@firesprinkler.org Subject: RE: Seismic Bracing - Clean Agent I saw that reference to ASME as well and made similar assumptions as you made. Yet it would mean a shop drawing review by the AHJ or the design engineer would bring in all

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Rod DiBona
st 08, 2011 12:31 PM To: sprinklerforum@firesprinkler.org Subject: RE: Seismic Bracing - Clean Agent So how did you interpret that since there are no specific bracing requirements or methods stated within NFPA 2001 other than to say it is to be "securely supported"? Craig L. Pra

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Craig.Prahl
nklerforum@firesprinkler.org Subject: RE: Seismic Bracing - Clean Agent Had a large clean agent project where we sent an RFI with the same question. Their response was that the bracing requirements of NFPA 2001 were sufficient. The sprinkler system had seismic and each brace even had to be modeled. ---

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Bill Brooks
craig.pr...@ch2m.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks Sent: Monday, August 08, 2011 1:31 PM To: sprinklerforum@firesprinkler.org Subject: Seismic Bracing - Clean Agent P

RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Rod DiBona
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks Sent: Monday, August 08, 2011 11:31 AM To: sprinklerforum@firesprinkler.org Subject: Seismic Bracing - Clean Agent Perhaps a bit off the reservation here but does anyone out there have some reason for the lack of