[Sprinklerforum] Re: Multiple sprinkler spacings

2024-03-22 Thread Dewayne Martinez
I think Todd is right too. No different than finding the spacing of a head next to the wall. Use the greater distance of either 2x the distance of the head off the wall or the spacing between that head and the next head in the line. Thank you, Dewayne Martinez Fire Protection Design Manager

[Sprinklerforum] Re: Exposed BlazeMaster

2024-03-22 Thread Dewayne Martinez
>From the Tyco BlazeMaster handbook [cid:image001.png@01DA7C2B.3D04E5A0] I know this isn't a system riser but the concept is the same. Maybe reach out to BlazeMaster and see what they say. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W

[Sprinklerforum] Re: FDC for Standpipe

2024-03-14 Thread Dewayne Martinez
Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm because of the pipe? From: John Denhardt Sent: Thursday, March 14, 2024 10:39 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: FDC for Standpipe Here is the

[Sprinklerforum] Re: Backflow In Stairwell

2024-01-15 Thread Dewayne Martinez
I think that the only pipe allowed in a stairwell has to be associated with the stairwell IE: standpipe or piping supplying sprinklers for the stairwell. We are on the 2015 IBC and I was flagged by the state reviewer for running a bulk pipe in the stairwell. Had to move it out into a closet.

[Sprinklerforum] Re: Braded Flex Drops

2023-12-18 Thread Dewayne Martinez
If braided flex and we can just swing the into a new tile then we reuse, otherwise we replace with new. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com<mailto:dmarti...@to

[Sprinklerforum] NFPA 13 (2022ed) sections 28.2.4.2.4 vs 28.2.4.2.5

2023-12-01 Thread Dewayne Martinez
When do you apply one vs the other? If I am interpreting correctly you apply 28.4.2.4 when you don't have the available floor area and 28.2.4.2.5 when you have the available floor area but not the minimum flow? Thanks, Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL

[Sprinklerforum] Re: [External]Re: Vertical lift modules

2023-03-20 Thread Dewayne Martinez
Thanks for the info. Gives me a place to start looking. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com> Ph: 262-522-7110 Cell: 4

[Sprinklerforum] Vertical lift modules

2023-03-17 Thread Dewayne Martinez
I have a customer who will be installing 2 VLM in there facility. Is there any guidance in NFPA or FM for sprinkler protection in these? All I can find online is for gas systems. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul

[Sprinklerforum] NFPA 22 minimum tank fill line size

2023-02-24 Thread Dewayne Martinez
NFPA 22, 2013 ed - Section 14.4 Tank will be filled by a well pump. Does the tank fill line have to be 2" minimum per 14.4.6.2 or can it be smaller if it meet the requirements of 14.4.2? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234

[Sprinklerforum] Re: [External]RE: Can OH II listed EC sprinklers be used for storage application?

2023-02-16 Thread Dewayne Martinez
Thanks Travis, I was just trying to convince myself that if it was still at or under the OH2 curve and I am allowed to design anywhere along that curve it could still be called OH2. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul

[Sprinklerforum] Can OH II listed EC sprinklers be used for storage application?

2023-02-15 Thread Dewayne Martinez
using extended coverage K14 sprinklers, 18x18 at OH 2 density. If I go up the OH2 curve to 2000 sq ft I get a 0.19/2000 density. Can I pick up the additional EC sprinklers for the 2000 sq ft at the required EHP for the OH 2 spacing and call it good if the calcs work? Thank you, Dewayne

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
I just received information from the Blazemaster rep that we should follow the rules for quick response upright sprinklers when using residential upright sprinklers. Thank you,   Dewayne Martinez Fire Protection Design Manager   TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
upright sprinklers with exposed CPVC. Thank you,   Dewayne Martinez Fire Protection Design Manager   TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI  53072 dmarti...@total-mechanical.com Ph:  262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com

Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
I don't see an option for using residential upright sprinkler on exposed CPVC pipe in any of the manufactures installation manuals. Am I missing something or is QR uprights my only option? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234

CMSA spacing obstruction rules

2021-10-01 Thread Dewayne Martinez via Sprinklerforum
uction? 8.11.5.3.4 – apply this for obstructions located >24in below the deflector unless they fall under 8.15.5.2.1.3 8.11.5.3.5 – Does this section supersede the requirements of 8.11.5.2.1.3 and 8.11.5.3.4 for anything running parallel to the branch lines? Thank you, Dewayne

RE: Does a remote free standing FDC require a valve pit?

2021-03-11 Thread Dewayne Martinez via Sprinklerforum
Do you wrap the ball drip in landscaping fabric to keep it from getting clogged with sediment? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI  53072 dmarti...@total-mechanical.com Ph:  262-522-7110 Cell: 414-406

Does a remote free standing FDC require a valve pit?

2021-03-10 Thread Dewayne Martinez via Sprinklerforum
bend and check to drain out the pipe. Anyone else have insight on this? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI  53072 dmarti...@total-mechanical.com Ph:  262-522-7110 Cell: 414-406-5208 http://www.total

Re: ESFR and Obstructed Construction

2020-10-06 Thread Dewayne Martinez via Sprinklerforum
How does the forum treat ESFR sprinklers when there is a wall added in the warehouse which creates the heads on one side to be too far away but when you add a new line it puts the ESFR sprinklers too close together? Some times there is that perfect storm where you can’t move the existing line

Re: Uprights in non combustible concealed space

2020-07-15 Thread Dewayne Martinez via Sprinklerforum
In Wisconsin we have done several NFPA 13 condo projects where the architect received approval to not sprinkler the attic when smoke and heat detection were installed. So not every state is interpreting it the same. On Wed, Jul 15, 2020, 12:51 Steve Leyton via Sprinklerforum <

RE: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Dewayne Martinez via Sprinklerforum
Thanks everyone for the input. My fitter brought this up to me and after I read the sections I was still not sure. John’s comment makes perfect sense. Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee

NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Dewayne Martinez via Sprinklerforum
Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler in a ceiling still required to one that prevents upward movement? Sections 9.2.3.4.4.1,9.2.3.5.2.2 Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL Mechanical* *Building* *Integrity* W234

RE: [EXTERNAL] Re: Combustible dust collector

2020-02-24 Thread Dewayne Martinez via Sprinklerforum
concern was that the collector itself was outside the building which would require a dry system which wasn’t figured. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522

Re: Combustible dust collector

2020-02-24 Thread Dewayne Martinez via Sprinklerforum
> > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Dewayne Martinez via Sprinklerforum > Sent: Tuesday, 25 February 2020 4:45 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Dewayne Martinez > Subject: Combustible dust collector &

Combustible dust collector

2020-02-24 Thread Dewayne Martinez via Sprinklerforum
is section 22.4 – spray applications using flammable or combustible materials. Anyone else have experience with this? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com

NFPA 13 - 2013ed ceiling pockets

2019-11-18 Thread Dewayne Martinez via Sprinklerforum
of the pockets are within the listed deflector distance of 12” they are considered protected and I can still apply the QR reduction. Anything other ideas…… Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI

Existing Dry system testing- chapter 25

2019-11-12 Thread Dewayne Martinez via Sprinklerforum
or is it up to the AHJ? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: cid:image003

RE: NFPA 13D (13ed) exposed basements

2019-06-12 Thread Dewayne Martinez
I should note that the basement compartment is larger than 600 sq ft and the span of the TJI’s are over 20ft. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522

NFPA 13D (13ed) exposed basements

2019-06-12 Thread Dewayne Martinez
We have a couple of houses with exposed basements and 12” TJI construction. 1. Is this considered “beamed ceiling” construction? 2. What is the best way to protect this space? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity

NFPA 13 (2013ed) figure 15.2.2

2019-05-20 Thread Dewayne Martinez
it would be higher density. Can anyone help me understand this? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http

RE: PRV By-pass

2019-01-10 Thread Dewayne Martinez
is the PReIV/PRedV? Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: A close up of a sign Description

RE: PRV By-pass

2019-01-10 Thread Dewayne Martinez
valve(with gauges on each side), tee down to a 2 ½” FHV, then a system control valve, check valve, riser manifold. I will probably just go with a globe UMC to simplify things. Sound ok? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity

NFPA 13 - mixing residential and QR sprinklers in dwelling units

2019-01-08 Thread Dewayne Martinez
sprinklers thought the dwelling unit else where would we need to pick up a 900sq ft remote area to account for the QR sprinkler? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total

Assisted living facility - residential sprinklers in corridors

2019-01-04 Thread Dewayne Martinez
for the staff to use. I was going to use residential sprinklers in the dwelling units, corridor and group areas and QR sprinklers in the offices and similar non-residential areas. Sound alright? Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234

Re: CPVC pipe passing thru ordinary interstitial space

2018-12-13 Thread Dewayne Martinez
I ran into this recently and it was pointed out to me that the floor assembly itself was UL rated fire assembly and if I ran the CPVC in the interstitial space it would have to comply with the OH rules of 400sf or less. I thought the same at first about it being protected per LH that it would

buried fdc ball drip?

2018-09-20 Thread Dewayne Martinez
). Can it be buried? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: A close up

RE: multi-height standpipes

2018-09-20 Thread Dewayne Martinez
Thanks for the information. I will do one set of calcs to size my PRV hose valves from floors 1-4 with the 3 standpipes flowing a total of 1000gpm and an additional set of calcs for floors 5-25 with 2-standpipes flowing a total of 750gpm. Dewayne Martinez Fire Protection Design Manager

multi-height standpipes

2018-09-19 Thread Dewayne Martinez
the matter even more the high standpipes would not have a pressure reducing hose valves in the calculation but the low standpipe would need one. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072

RE: [EXTERNAL] RE: PRV after pump discharge control valve

2018-07-20 Thread Dewayne Martinez
I think replacing the impeller for damage with the same one is fine. Replacing one with another size and making the unit not listed is not fine. Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total

RE: PRV after pump discharge control valve

2018-07-17 Thread Dewayne Martinez
75psi and bump up the pipe sizes to 8x6x3" grid. Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI  53072 dmarti...@total-mechanical.com Ph:  262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ -Original Message

RE: PRV after pump discharge control valve

2018-07-17 Thread Dewayne Martinez
My pump rep confirmed that changing the impeller was a no-go. He also had mentioned the VFD controller but was quoting a huge cost (108K...ouch). Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total

Re: PRV after pump discharge control valve

2018-07-14 Thread Dewayne Martinez
f, it's easy to rearange to solve for r!!! > > You should still install a spool piece I guess, but to pump it up only to let > the air out a couple feet later never has made sense to me. > > Maybe Nicky in NZ knows of something in the European Code that might shed a > different

PRV after pump discharge control valve

2018-07-13 Thread Dewayne Martinez
and I thought about leaving a space for a PRV to be installed downstream of the pump discharge valve to account for the future higher pressures. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072

RE: [EXTERNAL] RE: ESFR closer than 8'

2018-05-31 Thread Dewayne Martinez
? It’s great to say to insist that the walls are placed so this doesn’t happen but ½ of the time the wall is already built or can’t be placed conveniently because of outside windows. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul

RE: exterior roof overhang - omitting sprinkler protection

2018-05-24 Thread Dewayne Martinez
Thanks Brad, We are coming up with options. WI has just switch to the 2013ed but this one falls under 2007. Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414

exterior roof overhang - omitting sprinkler protection

2018-05-23 Thread Dewayne Martinez
in the estimate……. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: Consecutive Honors 2012-2017

RE: [EXTERNAL] Re: Drop In Anchors for Seismic

2018-05-07 Thread Dewayne Martinez
I believe Powers “snake” was also approved in cracked concrete. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total

RE: Supply calculation for manual-wet standpipe

2018-04-17 Thread Dewayne Martinez
I am not used to seeing this calc program so I may be looking at this wrong but I don’t see a water supply on this graph. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com

RE: Supply calculation for manual-wet standpipe

2018-04-17 Thread Dewayne Martinez
I initially put in a supply of 150psi at 1000gpm and then modify it until I get a 0 PSI cushion. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell

Supply calculation for manual-wet standpipe

2018-04-17 Thread Dewayne Martinez
taking the hard way around to solve what PSI is required at the FDC? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http

RE: Remote additional FDC

2018-04-03 Thread Dewayne Martinez
Not very easily. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: Consecutive Honors 2012

RE: Remote additional FDC

2018-04-03 Thread Dewayne Martinez
Thanks Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: Consecutive Honors 2012-2017

Remote additional FDC

2018-04-03 Thread Dewayne Martinez
) for no control valves between the FDC and standpipe system. Is there anything the precludes me from installing an additional FDC on the new addition to use the existing feed and satisfy 6.4.1? Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building

RE: Existing 3/4" outlets

2018-03-16 Thread Dewayne Martinez
That’s a thought.The problem is the original shell with 3/4" uprights with a pipe centerline of 12" below deck. No residential uprights in 3/4" and I thought residential pendant heads are not listed to be installed exposed? Dewayne Martinez Fire Protection Design Manager T

Existing 3/4" outlets

2018-03-15 Thread Dewayne Martinez
? Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: Consecutive Honors 2012-2017] -- next

RE: FDC & Pump

2018-02-02 Thread Dewayne Martinez
on the manifold. Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [image: Consecutive Honors 2012

RE: FDC & Pump

2018-02-02 Thread Dewayne Martinez
in over the years and I didn’t know it was wrong. I thought it was just like the individual system control valves on the manifold. Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total

RE: RE: Floating Ceilings

2017-12-15 Thread Dewayne Martinez
The attachment from this email is a virus so don’t click on it. I received one in my personal email. Thanks, Dewayne *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Bobby McCullough *Sent:* Friday, December 15, 2017 2:58 AM *To:*

RE: High-Rise with Secondary Water Supply

2017-12-07 Thread Dewayne Martinez
In Wisconsin the pipe before the BFP is plumbing if it’s a combined domestic/fire main otherwise it is all fire protection. If it’s fire protection we could use either brass, copper, stainless steel or galvanized steel (ASTM53 IE:Sch40) for our exposed metal pipe choices before the BFP.

RE: Fabric Ductwork - ESFR obstruction?

2017-11-14 Thread Dewayne Martinez
Received a unofficial response from NFPA that the collapsible fabric ducts do need ESFR sprinkler heads underneath if they don’t comply with the ESFR obstruction rules. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd

RE: Fabric Ductwork - ESFR obstruction?

2017-11-09 Thread Dewayne Martinez
*From:* Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Wednesday, November 08, 2017 5:06 PM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *S

Fabric Ductwork - ESFR obstruction?

2017-11-08 Thread Dewayne Martinez
NFPA 13, 07ed ESFR System What are the obstructions rules concerning a fabric supply duct installed below an ESFR system. The RTU will shut down and collapse the duct under any of the following conditions – Flow switch activation, heat detector and pull stations. I don’t think it should be

RE: Electric unit heaters

2017-10-17 Thread Dewayne Martinez
what would be the fuel source? What would actually be on fire? From the description I’m guessing the only combustible would be the insulation on the units’ wiring. On Tue, Oct 17, 2017 at 12:51 PM Dewayne Martinez < dmarti...@total-mechanical.com> wrote: NFPA 13 07ed Noncombustible p

Electric unit heaters

2017-10-17 Thread Dewayne Martinez
protection by the UH’s but I can’t find it in NFPA 13. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 *http://www.total

RE: NFPA 13 edition in Wisconsin

2017-10-17 Thread Dewayne Martinez
WI follows the 2009ed of the IBC so 2007ed of NFPA 13 is what we follow. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208

Central sprinkler butterfly valve

2017-10-16 Thread Dewayne Martinez
Does anyone have a cut sheet for an old Central sprinkler butterfly valve. I’m looking for parts for it. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262

RE: Schedule 10 vs Schedule 40 pipe

2017-10-04 Thread Dewayne Martinez
as they knew about it prior to fabrication. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 *http://www.total-mechanical.com/ <h

Radiant heat panels

2017-08-24 Thread Dewayne Martinez
information available. Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 *http://www.total-mechanical.com/ <http://www.to

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
:* Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Friday, August 11, 2017 9:12 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* Outrig

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Friday, August 11, 2017 9:12 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed) I had a AHJ question recent

Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
” required. Have I been wrong all these years? Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 *http://www.total-mechanical.com/ <h

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Dewayne Martinez
...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Friday, August 11, 2017 8:39 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* 10" pipe with 1.0 CRR Anyone know of 10in non

10" pipe with 1.0 CRR

2017-08-11 Thread Dewayne Martinez
Anyone know of 10in non-sch40 pipe that has a CRR of 1? Have a project where the EOR is insisting on this. They also have a 100lb maximum point load per hanger…..but that is a conversation for another day! Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical

ESFR with solid shelve racks

2017-08-02 Thread Dewayne Martinez
NFPA 13 (16ed) sections 16.1.6.6 and 16.1.6.8 I have a customer that installed solid shelve racks in part of a warehouse protected with ESFR sprinklers. NFPA 2016 allows this provided we follow section 16.1.6. What overhead density would I use for the ESFR sprinklers? Is 16.1.6.8 saying that

Galvanized pipe before backflow

2017-07-31 Thread Dewayne Martinez
Wisconsin requires when using steel pipe on the potable water side of the backflow preventer that it be ASTM A53 galvanized. Does ASTM A53 only come in Sch 40? Thanks, Dewayne ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

RE: Potter WLS

2017-06-15 Thread Dewayne Martinez
We use a lot of buried concrete tanks up here and typically use 2 sump floats (one for high and one for low alarms). The low one also operates a solenoid valve for the auto fill. Dewayne *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Richard

RE: Pump pads

2017-06-12 Thread Dewayne Martinez
I was taught it was a requirement of the pump manufactures for horizontal split case pumps. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *John Irwin *Sent:* Monday, June 12, 2017 11:11 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:*

Golf simulator

2017-06-08 Thread Dewayne Martinez
of the simulator and put sprinklers in the simulator itself. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Building** Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7110 Cell: 414-406-5208 *http

RE: Racks wider than 4ft...sprinklers needed below?

2017-04-21 Thread Dewayne Martinez
will act like an overhead door. I don’t feel we need additional protection here….Who Is right? *From:* Dewayne Martinez [mailto:dmarti...@total-mechanical.com] *Sent:* Friday, April 21, 2017 7:01 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* RE

RE: Racks wider than 4ft...sprinklers needed below?

2017-04-21 Thread Dewayne Martinez
Never mind, I found it in the definition of single row rack – 6ft wide. *From:* Dewayne Martinez [mailto:dmarti...@total-mechanical.com] *Sent:* Friday, April 21, 2017 6:54 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* Racks wider than 4ft

Racks wider than 4ft...sprinklers needed below?

2017-04-21 Thread Dewayne Martinez
NFPA 13 (07ed) I have an inspector that is requesting in-rack sprinklers for a single row rack located along an outside wall because the rack shelves are wider than 4ft (open shelve). The OHS is capable of protecting the racks W/O in-rack sprinklers. Is there something in NFPA to address this

RE: Sensing line fittings

2017-04-17 Thread Dewayne Martinez
We have used them and haven’t run into any problems. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Ben Young *Sent:* Monday, April 17, 2017 5:50 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* Sensing line fittings Is there any

RE: NFPA 13 dry system - residential sprinklers

2017-04-07 Thread Dewayne Martinez
for dry systems and is K5.6 or greater. Ed Kramer *From:* Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Thursday, April 06, 2017 8:13 AM *To:* sprinkle

RE: NFPA 13 dry system - residential sprinklers

2017-04-06 Thread Dewayne Martinez
in residential areas. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Apr 6, 2017, at 6:31 AM, Dewayne Martinez <dm

RE: NFPA 13 dry system - residential sprinklers

2017-04-06 Thread Dewayne Martinez
14 AM, Dewayne Martinez <dmarti...@total-mechanical.com> wrote: NFPA 13 (07ed) I have an existing 5th floor shell space that is installed as a light hazard dry system that has pipe in the shell space and in the attic. They are turning this floor into a dormitory (R-2). 1)Can I use listed reside

NFPA 13 dry system - residential sprinklers

2017-04-06 Thread Dewayne Martinez
11.3.1.1 or will I need to pick up 1950SF? What if there are incidental areas such as a laundry room, ect. in the same areas as the dorm rooms? 2)What would be the required trip time be per Table 7.2.3.6.1? 15sec for residential or 60sec for light hazard? Thanks, Dewayne Martinez Fire Protection

RE: Fire pump removal

2017-03-16 Thread Dewayne Martinez
rum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Thursday, March 16, 2017 6:35 AM *To:* sprinklerforum@lists.firesprinkler.org *Cc:* dmarti...@total-mechanical.com *Subject:* Fire pump removal I have a project in which there will be long term removal (3-6

Fire pump removal

2017-03-16 Thread Dewayne Martinez
I have a project in which there will be long term removal (3-6months)of the existing fire pump for building improvements. We need to keep the systems in service and this building is considered a high rise (110ft). What are some of my options? I thought possibly just using the incoming city

Dry system return bend - aux drain needed?

2017-03-03 Thread Dewayne Martinez
NFPA 13 (07ed) Section 8.16.2.5.3.3 states that aux drains are not required for pipe drops supplying dry-pendant sprinklers installed per 7.2.2 7.2.2 address both listed dry type sprinklers and pendant sprinklers installed on a return bend in a heated space I have someone questioning if aux

RE: Dwelling Unit Sprinkler Calc

2017-03-01 Thread Dewayne Martinez
NFPA 13 (10) section 11.3.1.1 also includes “adjacent”. What does this mean actually? 4 heads on the same line regardless of the walls or 4 heads in the same area but may be supplied from different lines? The pictures in the appendix are not very clear. Thanks, Dewayne *From:*

RE: Yard FDC Supply Line

2017-02-15 Thread Dewayne Martinez
See NFPA 13 (07ed) A8.17.2.3 *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *John Paulsen *Sent:* Tuesday, February 14, 2017 2:31 PM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* Yard FDC Supply Line Afternoon all! I am trying to

RE: Commodity class upgrade?

2017-02-14 Thread Dewayne Martinez
Travis, There is a section in the appendix which shows milk going from a Class I to Group A plastic with the addition of plastic crates. Maybe that’s where you saw it. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Roland Huggins *Sent:* Monday,

RE: Combustible concealed space under stair

2017-02-08 Thread Dewayne Martinez
.? Electrical equipment? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell *From:* Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez

Combustible concealed space under stair

2017-02-08 Thread Dewayne Martinez
NFPA 13 (07ed) section 8.15.1.2.9 Could this section be applied to a small combustible concealed space under stairs that is under 55 SF? Thanks, Dewayne ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

RE: NFPA-13R

2017-01-25 Thread Dewayne Martinez
I can see why the AHJ might want it on the 2nd floor corridor because of the “occupied” space above. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Travis Mack, SET *Sent:* Wednesday, January 25, 2017 9:26 AM *To:*

Pitot flow test kits

2017-01-19 Thread Dewayne Martinez
Anyone else have a problem with these new pitot flow test kits with the air “quick” couplings for the gauge rusting up and giving inaccurate readings? If so what have you done about it? I am thinking we should remove the gauge from the coupling after every use and blast it with WD-40 or the

Static pressure after backflow preventer

2017-01-11 Thread Dewayne Martinez
Is there really a pressure loss at 0gpm flow for backflow preventers like the curves show? I am trying to figure out my static pressure on a floor level with a fire pump at churn and it needs to be accurate. Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical

Re: How many standpipes do I calculate?

2016-12-27 Thread Dewayne Martinez
t; Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org > > > >> On Dec 27, 2016, at 7:04 AM, Dewayne Martinez >> <dmarti...@total-mechanical.com>

RE: How many standpipes do I calculate?

2016-12-27 Thread Dewayne Martinez
x: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack On 12/26/2016 10:42 AM, Dewayne Martinez wrote:

How many standpipes do I calculate?

2016-12-26 Thread Dewayne Martinez
I have a building that has two automatic wet standpipes and two automatic dry standpipes. Do I calculate them separately on the top floor or all together? My initial thought was all together because any of the hoses could be used to fight the fire on the top level. Thanks, Dewayne

RE: pipe heat trace

2016-12-01 Thread Dewayne Martinez
, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com *From:* Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne Martinez *Sent:* Wednesday, Novem