I think Todd is right too. No different than finding the spacing of a head
next to the wall. Use the greater distance of either 2x the distance of the
head off the wall or the spacing between that head and the next head in the
line.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
>From the Tyco BlazeMaster handbook
[cid:image001.png@01DA7C2B.3D04E5A0]
I know this isn't a system riser but the concept is the same. Maybe reach out
to BlazeMaster and see what they say.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W
Would a 5”x4” Storz be 750gpm because of the Storz connection size or 500gpm
because of the pipe?
From: John Denhardt
Sent: Thursday, March 14, 2024 10:39 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: FDC for Standpipe
Here is the
I think that the only pipe allowed in a stairwell has to be associated with the
stairwell IE: standpipe or piping supplying sprinklers for the stairwell. We
are on the 2015 IBC and I was flagged by the state reviewer for running a bulk
pipe in the stairwell. Had to move it out into a closet.
If braided flex and we can just swing the into a new tile then we reuse,
otherwise we replace with new.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com<mailto:dmarti...@to
When do you apply one vs the other? If I am interpreting correctly you apply
28.4.2.4 when you don't have the available floor area and 28.2.4.2.5 when you
have the available floor area but not the minimum flow?
Thanks,
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL
Thanks for the info. Gives me a place to start looking.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph: 262-522-7110
Cell: 4
I have a customer who will be installing 2 VLM in there facility. Is there any
guidance in NFPA or FM for sprinkler protection in these? All I can find
online is for gas systems.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul
NFPA 22, 2013 ed - Section 14.4
Tank will be filled by a well pump.
Does the tank fill line have to be 2" minimum per 14.4.6.2 or can it be smaller
if it meet the requirements of 14.4.2?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234
Thanks Travis,
I was just trying to convince myself that if it was still at or under the OH2
curve and I am allowed to design anywhere along that curve it could still be
called OH2.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul
using extended coverage K14 sprinklers, 18x18 at OH 2 density. If I go up the
OH2 curve to 2000 sq ft I get a 0.19/2000 density. Can I pick up the
additional EC sprinklers for the 2000 sq ft at the required EHP for the OH 2
spacing and call it good if the calcs work?
Thank you,
Dewayne
I just received information from the Blazemaster rep that we should follow the
rules for quick response upright sprinklers when using residential upright
sprinklers.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee
upright sprinklers with
exposed CPVC.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com
I don't see an option for using residential upright sprinkler on exposed CPVC
pipe in any of the manufactures installation manuals. Am I missing something
or is QR uprights my only option?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234
uction?
8.11.5.3.4 – apply this for obstructions located >24in below the deflector
unless they fall under 8.15.5.2.1.3
8.11.5.3.5 – Does this section supersede the requirements of 8.11.5.2.1.3
and 8.11.5.3.4 for anything running parallel to the branch lines?
Thank you,
Dewayne
Do you wrap the ball drip in landscaping fabric to keep it from getting
clogged with sediment?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406
bend and check to drain out the pipe. Anyone else have insight
on this?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total
How does the forum treat ESFR sprinklers when there is a wall added in the
warehouse which creates the heads on one side to be too far away but when you
add a new line it puts the ESFR sprinklers too close together? Some times
there is that perfect storm where you can’t move the existing line
In Wisconsin we have done several NFPA 13 condo projects where the
architect received approval to not sprinkler the attic when smoke and heat
detection were installed. So not every state is interpreting it the same.
On Wed, Jul 15, 2020, 12:51 Steve Leyton via Sprinklerforum <
Thanks everyone for the input. My fitter brought this up to me and after I
read the sections I was still not sure. John’s comment makes perfect
sense.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee
Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler
in a ceiling still required to one that prevents upward movement?
Sections 9.2.3.4.4.1,9.2.3.5.2.2
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL Mechanical*
*Building* *Integrity*
W234
concern
was that the collector itself was outside the building which would require
a dry system which wasn’t figured.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Dewayne Martinez via Sprinklerforum
> Sent: Tuesday, 25 February 2020 4:45 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Dewayne Martinez
> Subject: Combustible dust collector
&
is section 22.4 – spray applications using flammable or combustible
materials.
Anyone else have experience with this?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
of
the pockets are within the listed deflector distance of 12” they are
considered protected and I can still apply the QR reduction.
Anything other ideas……
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI
or is it
up to the AHJ?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: cid:image003
I should note that the basement compartment is larger than 600 sq ft and
the span of the TJI’s are over 20ft.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522
We have a couple of houses with exposed basements and 12” TJI construction.
1. Is this considered “beamed ceiling” construction?
2. What is the best way to protect this space?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity
it would be higher density. Can anyone help me understand this?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http
is the
PReIV/PRedV?
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: A close up of a sign Description
valve(with gauges on each side), tee down to a 2 ½” FHV, then a system
control valve, check valve, riser manifold. I will probably just go with a
globe UMC to simplify things. Sound ok?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity
sprinklers thought the
dwelling unit else where would we need to pick up a 900sq ft remote area to
account for the QR sprinkler?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total
for the staff
to use. I was going to use residential sprinklers in the dwelling units,
corridor and group areas and QR sprinklers in the offices and similar
non-residential areas. Sound alright?
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234
I ran into this recently and it was pointed out to me that the floor assembly
itself was UL rated fire assembly and if I ran the CPVC in the interstitial
space it would have to comply with the OH rules of 400sf or less. I thought
the same at first about it being protected per LH that it would
).
Can it be buried?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: A close up
Thanks for the information. I will do one set of calcs to size my PRV hose
valves from floors 1-4 with the 3 standpipes flowing a total of 1000gpm and
an additional set of calcs for floors 5-25 with 2-standpipes flowing a
total of 750gpm.
Dewayne Martinez
Fire Protection Design Manager
the matter even more the high standpipes would not have a pressure reducing
hose valves in the calculation but the low standpipe would need one.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
I think replacing the impeller for damage with the same one is fine.
Replacing one with another size and making the unit not listed is not fine.
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total
75psi and bump up the pipe sizes to 8x6x3" grid.
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
-Original Message
My pump rep confirmed that changing the impeller was a no-go. He also had
mentioned the VFD controller but was quoting a huge cost (108K...ouch).
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total
f, it's easy to rearange to solve for r!!!
>
> You should still install a spool piece I guess, but to pump it up only to let
> the air out a couple feet later never has made sense to me.
>
> Maybe Nicky in NZ knows of something in the European Code that might shed a
> different
and I
thought about leaving a space for a PRV to be installed downstream of the
pump discharge valve to account for the future higher pressures.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
? It’s great to say to insist that the walls are placed so this
doesn’t happen but ½ of the time the wall is already built or can’t be
placed conveniently because of outside windows.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul
Thanks Brad,
We are coming up with options. WI has just switch to the 2013ed but this
one falls under 2007.
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414
in the
estimate…….
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: Consecutive Honors 2012-2017
I believe Powers “snake” was also approved in cracked concrete.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total
I am not used to seeing this calc program so I may be looking at this wrong
but I don’t see a water supply on this graph.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
I initially put in a supply of 150psi at 1000gpm and then modify it until I
get a 0 PSI cushion.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell
taking the hard way around to solve what PSI is required at the FDC?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http
Not very easily.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: Consecutive Honors 2012
Thanks
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: Consecutive Honors 2012-2017
) for
no control valves between the FDC and standpipe system. Is there anything
the precludes me from installing an additional FDC on the new addition to
use the existing feed and satisfy 6.4.1?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building
That’s a thought.The problem is the original shell with 3/4" uprights
with a pipe centerline of 12" below deck. No residential uprights in 3/4"
and I thought residential pendant heads are not listed to be installed
exposed?
Dewayne Martinez
Fire Protection Design Manager
T
?
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: Consecutive Honors 2012-2017]
-- next
on the manifold.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[image: Consecutive Honors 2012
in
over the years and I didn’t know it was wrong. I thought it was just like
the individual system control valves on the manifold.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total
The attachment from this email is a virus so don’t click on it. I received
one in my personal email.
Thanks,
Dewayne
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Bobby
McCullough
*Sent:* Friday, December 15, 2017 2:58 AM
*To:*
In Wisconsin the pipe before the BFP is plumbing if it’s a combined
domestic/fire main otherwise it is all fire protection. If it’s fire
protection we could use either brass, copper, stainless steel or galvanized
steel (ASTM53 IE:Sch40) for our exposed metal pipe choices before the BFP.
Received a unofficial response from NFPA that the collapsible fabric ducts
do need ESFR sprinkler heads underneath if they don’t comply with the ESFR
obstruction rules.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd
*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Wednesday, November 08, 2017 5:06 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*S
NFPA 13, 07ed
ESFR System
What are the obstructions rules concerning a fabric supply duct installed
below an ESFR system.
The RTU will shut down and collapse the duct under any of the following
conditions – Flow switch activation, heat detector and pull stations.
I don’t think it should be
what would be the fuel source? What
would actually be on fire? From the description I’m guessing the only
combustible would be the insulation on the units’ wiring.
On Tue, Oct 17, 2017 at 12:51 PM Dewayne Martinez <
dmarti...@total-mechanical.com> wrote:
NFPA 13 07ed
Noncombustible p
protection by
the UH’s but I can’t find it in NFPA 13.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical*
*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
*http://www.total
WI follows the 2009ed of the IBC so 2007ed of NFPA 13 is what we follow.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
Does anyone have a cut sheet for an old Central sprinkler butterfly valve.
I’m looking for parts for it.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical*
*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262
as they knew about it prior to fabrication.
Dewayne Martinez
Fire Protection Design Manager
*TOTAL* *Mechanical*
*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
*http://www.total-mechanical.com/ <h
information available.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical*
*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
*http://www.total-mechanical.com/ <http://www.to
:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Friday, August 11, 2017 9:12 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* Outrig
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Friday, August 11, 2017 9:12 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)
I had a AHJ question recent
”
required. Have I been wrong all these years?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical*
*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
*http://www.total-mechanical.com/ <h
...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Friday, August 11, 2017 8:39 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* 10" pipe with 1.0 CRR
Anyone know of 10in non
Anyone know of 10in non-sch40 pipe that has a CRR of 1? Have a project
where the EOR is insisting on this. They also have a 100lb maximum point
load per hanger…..but that is a conversation for another day!
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical
NFPA 13 (16ed) sections 16.1.6.6 and 16.1.6.8
I have a customer that installed solid shelve racks in part of a warehouse
protected with ESFR sprinklers. NFPA 2016 allows this provided we follow
section 16.1.6. What overhead density would I use for the ESFR
sprinklers? Is 16.1.6.8 saying that
Wisconsin requires when using steel pipe on the potable water side of the
backflow preventer that it be ASTM A53 galvanized. Does ASTM A53 only come
in Sch 40?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
We use a lot of buried concrete tanks up here and typically use 2 sump
floats (one for high and one for low alarms). The low one also operates a
solenoid valve for the auto fill.
Dewayne
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Richard
I was taught it was a requirement of the pump manufactures for horizontal
split case pumps.
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *John Irwin
*Sent:* Monday, June 12, 2017 11:11 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:*
of the simulator and put sprinklers in the simulator itself.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical*
*Building** Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
*http
will act like an overhead door. I don’t feel we need additional
protection here….Who Is right?
*From:* Dewayne Martinez [mailto:dmarti...@total-mechanical.com]
*Sent:* Friday, April 21, 2017 7:01 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* RE
Never mind, I found it in the definition of single row rack – 6ft wide.
*From:* Dewayne Martinez [mailto:dmarti...@total-mechanical.com]
*Sent:* Friday, April 21, 2017 6:54 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* Racks wider than 4ft
NFPA 13 (07ed)
I have an inspector that is requesting in-rack sprinklers for a single row
rack located along an outside wall because the rack shelves are wider than
4ft (open shelve). The OHS is capable of protecting the racks W/O in-rack
sprinklers. Is there something in NFPA to address this
We have used them and haven’t run into any problems.
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Ben Young
*Sent:* Monday, April 17, 2017 5:50 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* Sensing line fittings
Is there any
for dry systems and is
K5.6 or greater.
Ed Kramer
*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Thursday, April 06, 2017 8:13 AM
*To:* sprinkle
in
residential areas.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Apr 6, 2017, at 6:31 AM, Dewayne Martinez <dm
14 AM, Dewayne Martinez <dmarti...@total-mechanical.com>
wrote:
NFPA 13 (07ed)
I have an existing 5th floor shell space that is installed as a light
hazard dry system that has pipe in the shell space and in the attic. They
are turning this floor into a dormitory (R-2).
1)Can I use listed reside
11.3.1.1 or will I need to pick up 1950SF? What if there are
incidental areas such as a laundry room, ect. in the same areas as the dorm
rooms?
2)What would be the required trip time be per Table 7.2.3.6.1? 15sec for
residential or 60sec for light hazard?
Thanks,
Dewayne Martinez
Fire Protection
rum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Thursday, March 16, 2017 6:35 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Cc:* dmarti...@total-mechanical.com
*Subject:* Fire pump removal
I have a project in which there will be long term removal (3-6
I have a project in which there will be long term removal (3-6months)of the
existing fire pump for building improvements. We need to keep the systems
in service and this building is considered a high rise (110ft). What are
some of my options? I thought possibly just using the incoming city
NFPA 13 (07ed)
Section 8.16.2.5.3.3 states that aux drains are not required for pipe drops
supplying dry-pendant sprinklers installed per 7.2.2
7.2.2 address both listed dry type sprinklers and pendant sprinklers
installed on a return bend in a heated space
I have someone questioning if aux
NFPA 13 (10) section 11.3.1.1 also includes “adjacent”. What does this
mean actually? 4 heads on the same line regardless of the walls or 4 heads
in the same area but may be supplied from different lines? The pictures in
the appendix are not very clear.
Thanks,
Dewayne
*From:*
See NFPA 13 (07ed) A8.17.2.3
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *John Paulsen
*Sent:* Tuesday, February 14, 2017 2:31 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* Yard FDC Supply Line
Afternoon all!
I am trying to
Travis,
There is a section in the appendix which shows milk going from a Class I to
Group A plastic with the addition of plastic crates. Maybe that’s where
you saw it.
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Roland
Huggins
*Sent:* Monday,
.?
Electrical equipment?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
NFPA 13 (07ed) section 8.15.1.2.9
Could this section be applied to a small combustible concealed space under
stairs that is under 55 SF?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
I can see why the AHJ might want it on the 2nd floor corridor because of
the “occupied” space above.
*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Travis Mack,
SET
*Sent:* Wednesday, January 25, 2017 9:26 AM
*To:*
Anyone else have a problem with these new pitot flow test kits with the air
“quick” couplings for the gauge rusting up and giving inaccurate readings?
If so what have you done about it? I am thinking we should remove the
gauge from the coupling after every use and blast it with WD-40 or the
Is there really a pressure loss at 0gpm flow for backflow preventers like
the curves show? I am trying to figure out my static pressure on a floor
level with a fire pump at churn and it needs to be accurate.
Thanks,
Dewayne Martinez
Fire Protection Design Manager
*TOTAL** Mechanical
t; Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>> On Dec 27, 2016, at 7:04 AM, Dewayne Martinez
>> <dmarti...@total-mechanical.com>
x: 866-430-6107
email:tm...@mfpdesign.com
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack
On 12/26/2016 10:42 AM, Dewayne Martinez wrote:
I have a building that has two automatic wet standpipes and two automatic
dry standpipes. Do I calculate them separately on the top floor or all
together? My initial thought was all together because any of the hoses
could be used to fight the fire on the top level.
Thanks,
Dewayne
, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Dewayne
Martinez
*Sent:* Wednesday, Novem