RE: 2'x4' Light Obstruction

2010-03-29 Thread Paul Pinigis
below them for the same reason (the are under 4' wide). Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Monday, March 29, 2010 3:13 PM

RE: Accidental Fusing

2010-02-05 Thread Paul Pinigis
Brad, Are you a lawyer? Paul From: sprinklerforum-boun...@firesprinkler.org on behalf of Brad Sent: Fri 2/5/2010 1:02 PM To: sprinklerforum@firesprinkler.org Subject: Accidental Fusing Do any contractors have experience with heads fusing 'accidentally'?

RE: standpipe for attic?

2009-11-11 Thread Paul Pinigis
Per section 1509.2 of the 2006 IBC, a penthouse or rooftop enclosure can be up to 1/3 of the area of the roof. Over that and it is a floor. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: Chance to Make a Difference in Military Standards

2009-10-09 Thread Paul Pinigis
Bill, What section prohibits the placement of risers on exterior walls? Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks Sent: Friday, October 09

RE: Virginia Zero Sq. Ft. policy? yes or no

2009-07-31 Thread Paul Pinigis
Virginia adopts the IBC with some amendments, but there is no zero sq. ft. policy. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent

RE: Hydrant Flow test results

2009-06-23 Thread Paul Pinigis
Any single-hydrant test is questionable to begin with, but if two tests are done they should yield identical graphs. Pitot pressures of less than 10 psi are generally unacceptable. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun

RE: UAE, Saudi, Codes and standards and component certifications

2009-05-11 Thread Paul Pinigis
We often hire a local architect to assist in code evaluations to ensure local-code compliance. I do have the fire code of Taiwan if anyone speaks Mandarin. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Branch line insulation

2009-04-24 Thread Paul Pinigis
Insulation on a pipe with non-flowing water is pointless (except for temporary exposures to low temperatures). Insulation can only slow the transmission of heat from the pipe, it does nothing to produce heat. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From

RE: Walk-in cooler

2009-04-23 Thread Paul Pinigis
What you have described is a room, and just like every other room in a sprinkered building it must also be sprinklered. That fact that it is cold in there is irrelevant. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
It depends upon the distance between buildings and the percent of open wall space under the roof. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen

RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
area for the system. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen Purvis Sent: Monday, March 23, 2009 10:05 AM To: sprinklerforum@firesprinkler.org

RE: Possible IBC question

2009-03-23 Thread Paul Pinigis
One last thing to keep in mind is that some water companies demand separate services if they are considered separate buildings; that supersedes the requirements of NFPA 13. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun

RE: Pipe Labeling

2009-03-05 Thread Paul Pinigis
On F-Troop, FIRE WATER was a beverage. :) Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Thursday, March 05, 2009 1:54 PM

RE: PE Peer Review

2009-02-26 Thread Paul Pinigis
was littered with statements-of-the-obvious that have nothing to do with deficiencies in your design like: comply with NFPA 13, follow the obstruction rules, take an umbrella if its raining... and all of the other fluff and filler they use to make their reviews appear extensive. Paul Pinigis, P.E. Life

RE: underground pre-action piping

2009-02-20 Thread Paul Pinigis
I would suggest mechanical-joint cement-lined ductile iron, but I do not know how you are going to drain it short of putting in a pit. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: * Possible Spam *Re: Bedbug Treatment

2009-02-06 Thread Paul Pinigis
I agree that it would be a waste to simply dispose of perfectly good sprinklers, and I personally would have no problem with someone reusing them for such an application. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Sprinklered vs Sprinkled

2009-01-15 Thread Paul Pinigis
Yes, I have heard it many times here in Virginia, and always find it amusing. Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of bill.bro...@brooksfpe.com

RE: another fire - this will be interesting

2009-01-07 Thread Paul Pinigis
engineer or the plumbing engineer showing their detailed designs. I would like to see equal treatment; the HVAC engineers should show a hatch pattern on the floor plan with a note that says deign ductwork to provide a comfortable environment.. Paul Pinigis, P.E. Life Safety Department Head

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
Very well said John. This is exactly the approach that we take; we look at the building or project holistically and our fire protection engineers direct the architect, mechanical, electrical, structural, telecom, etc. to ensure coordination and compliance. Paul Pinigis, P.E. Life Safety

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
We have 5 registered FPEs (not turd-herders pretending to be FPEs) and 5 EITs who will get registered as they become eligible. Most of our design work is done by our designers (two Level IV, and one Level II). Our engineers are responsible for the ENGINEERING activities. Paul Pinigis, P.E. Life

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
There is your problem! You have electrical doing fire alarm and mechanical doing sprinkler!!! You just defined the need for a qualified FPE to perform those functions (and many more). Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun

RE: another fire - this will be interesting

2009-01-06 Thread Paul Pinigis
engineering (his previous responsibility was designing industrial valves). Paul Pinigis, P.E. Life Safety Department Head -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Tuesday, January 06

RE: Residential Sprinkler Ordinances

2008-08-15 Thread Paul Pinigis
It appears that all jurisdictions that adopt NFPA 101 have, either intentionally or inadvertently, adopted the requirement for sprinkler protection in all one- and two-family homes. The only state that comes to mind as having adopted NFPA 101 is West Virginia; and I do not know if they are

RE: NFPA 101 Dwelling Unit Sprinklers

2008-08-12 Thread Paul Pinigis
That is really funny! I read it the same way. If you provide party walls between the townhouses they become single family homes and require sprinkler protection, but if you don't they are garden apartments and do not require sprinklers. I would be very interested to know the logic behind this

RE: Shelf Storage

2008-08-12 Thread Paul Pinigis
Keeping it brief Bill? Paul Pinigis Hankins and Anderson -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Tuesday, August 12, 2008 2:12 PM To: sprinklerforum@firesprinkler.org Subject: Shelf Storage

RE: Soleniod valve

2008-08-11 Thread Paul Pinigis
I don't think that you will find a solenoid valve that is listed as preaction valve, but the engineer of record should be able to point you to one if it exists and was the basis of his design. Preaction valves do have solenoid valves in them, but the solenoid is not usually listed for the purpose

RE: Floating Ceilings

2008-08-05 Thread Paul Pinigis
Rick, I agree with you, you no longer have a noncombustible concealed space above the ceiling. When we see architects attempt this at the design stage we usually steer them away from the cloud ceiling; when we cannot, we sprinkler above and below the ceiling (obstruction). Paul J. Pinigis,

RE: Stair shafts

2008-07-31 Thread Paul Pinigis
Most carpeting meets the definition of non-combustible, but I would suggest checking the manufacturers cut sheet to verify. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Margaret Zabel Sent: Thursday,

RE: Water Supply

2008-07-30 Thread Paul Pinigis
I would suggest redoing the flow test and using a playpipe for better accuracy. If the first test was done with an open hydrant butt and a factor or 0.9, you may find that the estimate was too conservative. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From:

RE: Water Supply

2008-07-30 Thread Paul Pinigis
I just re-read your original question. If I read it correctly, you indicate that your demand point is below the curve, but the flow measured during the test was less than the demand flow of your system. As long as you are below the curve you are fine. The amount of flow at the time of the

RE: Deperming Pier

2008-07-24 Thread Paul Pinigis
Please direct your questions about this installation to the engineer of record, Eric Shelton, P.E. Thank you, Paul J. Pinigis, P.E. Chief Life Safety Engineer Hankins and Anderson -Original Message- From: [EMAIL PROTECTED] on behalf of Kurt Kingston Sent: Thu 7/24/2008 10:51 AM To:

RE: Fire Flow Calculation

2008-07-23 Thread Paul Pinigis
Nope, if you have a building that is not sprinklered in accordance with NFPA 13 (and you don't because there are unsprinklered areas beyond those that are allowed to be unsprinklered by NFPA 13) you have an unsprinklered building. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original

RE: Institutional Sprinklers

2008-07-14 Thread Paul Pinigis
How about putting some indelible orange ink in the line so that the next moron who opens the sprinkler becomes an oompa loompa? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Monday,

RE: Backflow device and steel pipe

2008-07-02 Thread Paul Pinigis
But, ductile iron IS ferrous pipe! Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski Sent: Wednesday, July 02, 2008 8:21 AM To: sprinklerforum@firesprinkler.org Subject: RE: Backflow device

RE: PIV 40ft from Building

2008-06-18 Thread Paul Pinigis
As the story was told to me, this dates back to the first iron-framed buildings with brick exterior walls. The buildings were generally walk-ups (pre-elevator days) so they were up to four stories tall. The problem was that the iron would expand in a fire and push outward on the walls until the

RE: Sectional Valves...

2008-05-21 Thread Paul Pinigis
If the closure of those valves will impair the operation of the system (which I believe they will) they need to be monitored. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of RFI - Bismarck Sent:

RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
Look at the cut sheet on the BFP. Some BFPs require a significant amount of pressure to open at very low flows. For example, an 12 Ames 2000SS requires almost 6 psi to operate at very low flow so it can sit there all day with an upstream pressure nearly 6 psi higher than the system side

RE: Change in static pressure

2008-05-09 Thread Paul Pinigis
was flown. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, May 09, 2008 1:22 PM To: sprinklerforum@firesprinkler.org Subject: RE: Change in static pressure Look at the cut sheet on the BFP. Some BFPs require a significant

RE: Hay Bale/Cube Storage

2008-03-17 Thread Paul Pinigis
Class III, ordinary combustibles. See chapter 14 of the 2007 NFPA 13 for design density curves. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr Sent: Sunday, March 16, 2008 5:28 PM To: American

RE: Fuel Tank Rooms

2008-03-10 Thread Paul Pinigis
Why? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Denhardt Sent: Monday, March 10, 2008 2:10 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fuel Tank Rooms NFPA 13 - 2007 I would try

RE: Fuel Tank Rooms

2008-03-10 Thread Paul Pinigis
I would agree with OH2 (or even OH1). It is a combustible liquid in a closed system. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Phelan Sent: Monday, March 10, 2008 1:51 PM To:

RE: BASIC HYDRAULICS

2008-02-28 Thread Paul Pinigis
Elevation still affects the pressure in a closed system. If the water is static in a pressurized system the pressure is the same throughout the system only at a constant elevation. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED]

RE: Dormitory Bunk Beds

2008-02-26 Thread Paul Pinigis
8.5.5.3.2 Sprinklers shall not be required under obstructions that are not fixed in place such as conference tables. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of G. Tim Stone Sent: Tuesday, February

RE: Gaggle of closets

2008-02-22 Thread Paul Pinigis
Don't you just love it when the letter of the code works in your favor. I really don't think that this is what the NFPA 13 committee had in mind when they developed that section. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: General Seismic Question

2008-02-20 Thread Paul Pinigis
1. No, that is the responsibility of the engineer and the project design team. 2. Yep, that is a clear change order. 3. Check your contract for this one. He most likely has to pay for work done and materials fabricated. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original

RE: Diesel vs Electric

2008-02-15 Thread Paul Pinigis
We have found that a diesel pump alone is more cost effective than an electric with a gen set. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Charles Thurston Sent: Friday, February 15, 2008 7:32 AM To:

RE: Re[2]: Who's the most important person?

2008-02-06 Thread Paul Pinigis
important person? So why is it that we're always wondering why we have so many idiot clients ... ?? Oh, never mind. :o) Steve Leyton Protection Design Consulting -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, February 06

RE: 3 alarm Fire @ Monte Carlo now in las vegas

2008-01-25 Thread Paul Pinigis
It looks that way. But WHY? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... Sent: Friday, January 25, 2008 3:11 PM To: sprinklerforum@firesprinkler.org Subject: 3 alarm Fire @ Monte Carlo now in

RE: MIC Testing

2008-01-18 Thread Paul Pinigis
! -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, January 18, 2008 6:06 AM To: sprinklerforum@firesprinkler.org Subject: RE: MIC Testing There is a forensic metallurgist in Northern Virginia that I have used a few times. I am looking

RE: MIC Testing

2008-01-18 Thread Paul Pinigis
There is a forensic metallurgist in Northern Virginia that I have used a few times. I am looking for his card, but no luck yet. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent:

RE: One Fire Pump Serving Multiple Buildings

2008-01-17 Thread Paul Pinigis
I have done this several times. It is analogous to single pump house feeding a campus, but you happen to have the pump in one of the protected buildings instead. Just as with a pump house, you assume a single fire condition. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original

RE: Great Forum Advice...

2008-01-16 Thread Paul Pinigis
Maybe we can get the Union and the class-action lawyer listed on the State Department's list of terrorist organizations. It sounds like their tactics are awfully similar to those of other extremists. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL

RE: Room Design

2007-12-21 Thread Paul Pinigis
If the doors are open at the time of your visit, I think it is safe to assume that they will be propped open at other times as well (unless of course they were temporarily propped open to move equipment in or out). Merry Christmas everyone! Paul J. Pinigis, P.E. Chief Life Safety Engineer

RE: Room Design

2007-12-21 Thread Paul Pinigis
I am not sure if I understand your question completely, but here is my attempt at an answer. The remote area is the actual physical area and not the hydraulic area. For example, consider a 22'x22' room with four sprinklers on 14' centers, the actual physical area is 484 sq. feet, but the

RE: Standpipe Requirements

2007-12-20 Thread Paul Pinigis
That is going to be in the building code. If you are using the IBC, the height of the building dictates the necessity of standpipes. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent:

RE: Flow test effective point.

2007-12-14 Thread Paul Pinigis
Yes, you must correct for elevation. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Thursday, December 13, 2007 5:52 PM To: sprinklerforum@firesprinkler.org Subject: Flow test

RE: Dick Patton

2007-12-12 Thread Paul Pinigis
Yes, I got a copy of his report from the 1970s. The current cost, with inflation, is actually $1.71 per square foot, but he took credit for reducing the amount of fireproofing on the structure as a reduction in the cost of his system. He provided no details to show a difference between his

RE: Dick Patton

2007-12-12 Thread Paul Pinigis
:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, December 12, 2007 1:57 PM To: sprinklerforum@firesprinkler.org Subject: RE: Dick Patton Yes, I got a copy of his report from the 1970s. The current cost, with inflation, is actually $1.71 per square foot, but he took credit for reducing

RE: Wow

2007-11-21 Thread Paul Pinigis
I reviewed some of his writings, and he has an obvious bias against just about everything.except heat detectors. I wonder if he is one of those guys who sells the wind-up heat detectors? Most of his statistics appear to be unfounded, and unsubstantiated. He is also part of an organization

RE: Wow

2007-11-21 Thread Paul Pinigis
I just got a return email from Mr. Patton. He is going to send me a copy of his report on the 35 cent design. I will disseminate what I learn from it to the forum in a couple of weeks. I am imagining thousands of water balloons tied to the ceiling, but I think the labor for that might exceed

RE: 13-R Anti freeze conversions

2007-10-25 Thread Paul Pinigis
I assume that these systems are not CPVC since CPVC is incompatible with most antifreeze. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ford, Charles Sent: Thursday, October 25, 2007 3:38 PM To:

RE: UNDERGGROUND FIRE MAIN TESTING

2007-10-11 Thread Paul Pinigis
Pressure is pressure, but do you really want to test the integrity of plastic fittings with a compressible gas? A failure could produce a most interesting rocket from a piece of pipe. If you must use a gas, why nitrogen, why not compressed air (not suggesting that either is a good idea)? Paul

RE: [NJFireSafety] NASFM Code Enforcement Bulletin again

2007-10-10 Thread Paul Pinigis
According to this approach, my office is an H occupancy. There is not separation of my office from the rest of the spaces on this floor and we have hundreds of chairs and several couches. I do believe that we have more than 250 pounds of polyurethane foam in the fire area. Now I am scared, I

RE: Owner's Information Certificate

2007-08-03 Thread Paul Pinigis
That depends upon the source of that information that he has interpreted. His property and casualty insurer (FM, IRI, etc.) may have emphasized the property protection aspects of an NFPA 13 system since they do not insure human life. Paul J. Pinigis, P.E. Chief Life Safety Engineer

RE: Telling an AHJ No ?

2007-08-01 Thread Paul Pinigis
We have an AHJ here who has been elevated to deity status by every spineless architect, engineer, and owner that bends to his every whim and wish. He is generally very knowledgeable, but not always correct, and does not appreciate having his knowledge questioned. He refused to even look at a

RE: Interpretation of nfpa 13, 8.1.1(1)

2007-08-01 Thread Paul Pinigis
Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul

RE: Interpretation of nfpa 13, 8.1.1(1)

2007-08-01 Thread Paul Pinigis
- 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, August 01, 2007 12:21 PM To: sprinklerforum@firesprinkler.org Subject: RE: Interpretation of nfpa 13, 8.1.1(1) If there is nothing

RE: Corps of Engineers Grv'd Cplg Spec

2007-07-31 Thread Paul Pinigis
The client paid for the design, but not the cost of producing multiple sets of drawings to be sent out to bidders. The small fee that is charged is not for the design, but for the paper output. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED]

RE: Corps of Engineers Grv'd Cplg Spec

2007-07-31 Thread Paul Pinigis
: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, July 31, 2007 7:44 AM To: sprinklerforum@firesprinkler.org Subject: RE: Corps of Engineers Grv'd Cplg Spec The client paid for the design, but not the cost of producing multiple sets of drawings to be sent out

RE: 10psi Saftey Factor

2007-07-23 Thread Paul Pinigis
Why? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Sunday, July 22, 2007 1:39 PM To: sprinklerforum@firesprinkler.org Subject: 10psi Saftey Factor

RE: IDOD Dry pipe systems

2007-07-12 Thread Paul Pinigis
IDOD is just a high-quality galvanized pipe that has a nice alloy layer of zinc and steel on the surface because the pipe is heated to the same temperature as the zinc bath before it is dipped. There is no flaking of the zinc coating that you get when you roll grove lower quality pipe (e.g. stuff

RE: IDOD Dry pipe systems

2007-07-12 Thread Paul Pinigis
IDOD is the product name for a galvanized pipe product. The IDOD came from Inside Diameter, Outside Diameter since both surfaces are galvanized. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of

RE: Sprinkler Success Story

2007-06-28 Thread Paul Pinigis
Dan, Is this a dry pipe or pre-action system? Did the pipe happen to be made in China? Was there any testing for the presence of the microbes associated with MIC? What type of sprinklers were these? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL

RE: Sprinkler Success Story

2007-06-28 Thread Paul Pinigis
, 2007 10:44 AM To: sprinklerforum@firesprinkler.org Subject: RE: Sprinkler Success Story This is a standard wet type system. Dan Arbel Tel: 972-4-8243337 Fax: 972-4-8243278 M: 972-52-2810593 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent

RE: Gang Drain for Attic Dry System

2007-06-28 Thread Paul Pinigis
Yes, unless you put a drain valve on the end of each branch line to facilitate drainage of each line individually. Could be expensive. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]

RE: Steam Room

2007-06-22 Thread Paul Pinigis
What would be your justification for not protecting that room? I can not find anything that would permit omission of sprinklers. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent:

RE: Steam Room

2007-06-22 Thread Paul Pinigis
-246-0164 fax 865-246-1084 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, June 22, 2007 2:13 PM To: sprinklerforum@firesprinkler.org Subject: RE: Steam Room What would be your justification for not protecting that room? I can

RE: Biodiesel mfg

2007-06-14 Thread Paul Pinigis
Biodiesel is vegetable oil, and likely a Class IIIB combustible liquid. You should question the classification considering that the flash point of vegetable oil is very high. The following is from an FM document: The closed cup flash point of the tested vegetable oil was 450°F (232°C) Even

RE: Test

2007-06-08 Thread Paul Pinigis
Ding. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ray Schmid Sent: Friday, June 08, 2007 7:08 AM To: sprinklerforum@firesprinkler.org Subject: Test Ray Schmid, P.E. Principal Koffel

RE: FDC check valves

2007-05-31 Thread Paul Pinigis
In my 1983 edition the requirement is listed and there is a bar next to the section indicating that it was either new or changed. But, there are other references to the check valve that don't indicate changes, so the requirement definitely predates 1983. Paul J. Pinigis, P.E. Chief Life Safety

RE: Combustible Construction Stair Ways

2007-05-23 Thread Paul Pinigis
(1) the presence of the gypsum board does not change the construction to non-combustible. (2) good question, that one is not clear to me. My initial response would be yes, but the requirement is vague. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL

RE: Cycling Systems

2007-05-17 Thread Paul Pinigis
Are you referring to the Viking Firecycle system? If so, they seem to be most useful on projects with nervous electrical engineers. I have proposed them on data center projects just to get electrical engineers to stop hyperventilating at the thought of having a sprinkler system discharge in

RE: Carpet Padding Commodity Classification

2007-05-16 Thread Paul Pinigis
It is an expanded plastic, but you would need to know what materials are used to be any more specific. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Smith, Steven D. (CSFD) Sent: Wednesday, May 16, 2007

RE: Pockets or just plain Obstructions

2007-05-15 Thread Paul Pinigis
Check your math, but first convert 14 to 1.167'. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Coastal Sent: Tuesday, May 15, 2007 8:40 AM To: sprinklerforum@firesprinkler.org Subject: Pockets or just

RE: Re[2]: Pockets or just plain Obstructions

2007-05-15 Thread Paul Pinigis
Thurston Sent: Tuesday, May 15, 2007 9:57 AM To: Paul Pinigis Subject: Re[2]: Pockets or just plain Obstructions Hello Paul, Got my coffee and construction calculator working now and it looks like 113.5556 cubic feet Tuesday, May 15, 2007, 8:44:52 AM, you wrote: Check your math, but first

RE: Article on Sprinkler Recall

2007-05-08 Thread Paul Pinigis
a round of golf below 85 on Saturday. Methinks Shakespeare is taken out of context too often; I wouldn't be here otherwise. glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, May 04, 2007 10:45 AM To: sprinklerforum

RE: Margarine

2007-05-07 Thread Paul Pinigis
I would suggest storing the margarine with huge amounts of popping corn. It may not control the fire, but it would be mighty tasty. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Monday,

RE: Article on Sprinkler Recall

2007-05-04 Thread Paul Pinigis
This is America, you can be sued by anyone for anything as long as there are scum-bag lawyers salivating at the prospect of making a dollar. We should have followed Shakespeare's advice and killed all of the lawyers. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message-

RE: Manual wet standpipes

2007-04-10 Thread Paul Pinigis
If there is city water available, include it too. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Tuesday, April 10, 2007 11:23 AM To: SprinklerFORUM Subject: Manual wet standpipes

RE: Roof Deck

2007-04-09 Thread Paul Pinigis
I should have studied! I failed! Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack Sent: Monday, April 09, 2007 2:03 PM To: sprinklerforum@firesprinkler.org Subject: Roof Deck Ok..this may be

RE: C urious

2007-03-30 Thread Paul Pinigis
I would suggest that you ask the AHJ for the section that you are violating. Are you violating Table 8.3.2.5(a)? Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Friday, March 30, 2007

RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
I don't know if this is what you are looking for, but if you use a sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to minimize pressure demand) is 106 square feet. Maybe a 10 x 10.5 foot spacing. The approach that you take will differ depending upon the ALL of the factors

RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
phone 704.948.3507 fax -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 9:46 AM To: sprinklerforum@firesprinkler.org Subject: RE: Selecting Heads For a New System I don't know if this is what you

RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
If your required density is 0.20 gpm/sq. ft., a 5.6 k-factor will require 21.55 psi minimum for 130 sq. ft. With the flow data that you described this may be a waste of precious pressure (say that three times fast!). Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original Message-

RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
pressure)? Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis

RE: Selecting Heads For a New System

2007-03-27 Thread Paul Pinigis
:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 10:31 AM To: sprinklerforum@firesprinkler.org Subject: RE: Selecting Heads For a New System If you have an ECOH with a k-factor of 14 it could be done. I like that approach. Paul J. Pinigis, P.E. Chief Life Safety

RE: Seed Corn

2007-03-27 Thread Paul Pinigis
I would simply consider these to be a plastic commodity to start with. The fire is going to be initially fuelled by the totes without regard to what is inside them. The fire is only going to see plastic as the fire begins to grow. Paul J. Pinigis, P.E. Chief Life Safety Engineer -Original

RE: owners information certificate

2007-03-20 Thread Paul Pinigis
Don't fool yourself into believing that you can escape liability. His lawyers will claiming that you are the expert and you knew about their future plans and still put in an inappropriate system. Everything changes after a loss. Paul Pinigis -Original Message- From: [EMAIL PROTECTED

RE: owners information certificate

2007-03-20 Thread Paul Pinigis
of breaking the law, albeit inadvertently. I feel better now, their family is now safe. glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 20, 2007 12:12 PM To: sprinklerforum@firesprinkler.org Subject: RE: owners

RE: Fill times

2007-03-20 Thread Paul Pinigis
(Volume of the pipe) / (pumper truck pump rate in GPM) = time in minutes. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Tuesday, March 20, 2007 3:17 PM To: sprinklerforum@firesprinkler.org Subject: Fill times Does anyone know where I