There was nothing to suggest water hammer. Water hammer resulting from a
pump start is unlikely in sprinkler system piping. Even if there is a
water hammer problem, it's something you want to know because it's easy
to fiz.When you do see water hammer from a fire pump, it usually happens
in und
was the system ever tested with a water hammer produced by the pump
so has to ensure everything was good and tight? Water hammer is a
much bigger concern than static pressure. I certainly agree with
checking it several times but when do you stop pounding things week
in and week out?
The
zackery The more appropriate way to word it is that it makes NO
SENSE to unnecessarily expose to system to additional stress. The TC
has stated that it is not necessary to test such small modifications
to the system beyond the working pressure.
Roland
On Mar 8, 2007, at 3:35 PM, Greg Mc
Plastic cable-ties (with company logos or seals at the end) are becoming
more acceptable today, easy to replace at minimal cost, recyclable, and
a lot safer than lead to process!
Jack C Kilavuz
Risk Engineer
E mailto:[EMAIL PROTECTED]
-Original Message-
From: [EMAIL PROTECTED]
[mail
A real-world example:
Just a couple of years ago there was a situation at an auto parts
warehouse. Fully sprinklered, adequate for the commodity and storage
arrangement. Water supplied by a fire pump. Because of concerns that
system might leak, even though it was relatively new with no sign
Better to find system defects now than during a fire, make a disclaimer as
noted before: my work leaks - then I fix it, others work leaks pay me to fix
it.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, March 08, 2007 6:35 PM
I agree with Garth with everything except we ALL have one huge
unknownwho has worked on the system since it was new and the system was
put in service? Has anyone changed a leaking head, relocated a head or etc
and it was tested then? We have seen sprinklers in service that were slow
dripping an
The vast majority (99%) of all of the sprinkler system
control valves at my former company were locked open
with padlocks and chains. However, there were few
occasions where a control valve was sealed closed for
manual operations (dust collectors). These seals were
made of metal and are normally us
The Fitter makes good sense.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Thursday, March 08, 2007 5:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: What I'm Hearing About Hydrostatic Testing
The owner may not care but th
Seton sells lead (which you may want to avoid unless you hand out MSDS for
each seal) and stainless steel seals and a crimping tool.
Garth
a fitter
- Original Message -
From: "Jay Stough" <[EMAIL PROTECTED]>
To: "AFSA Sprinkler Forum"
Sent: Thursday, March 08, 2007 2:15 PM
Subject: Valv
Please re-enable my membership.
Thank you.
mario berrios
[EMAIL PROTECTED]
AOL now offers free email to everyone. Find out more about what's free from
AOL at AOL.com.
___
Sprinkler
AMEN
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Garth W.
Warren
Sent: Thursday, March 08, 2007 3:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: What I'm Hearing About Hydrostatic Testing
The owner may not care but the firefighters that wer
The owner may not care but the firefighters that were expecting the water at
the fire area would sure be disappointed. If we are actually scared our
systems are going to blow-up during pressurization, like will normally
happen during firefighter response, then we are offering a false sense of
secu
BULLSEYE
Roland
On Mar 8, 2007, at 11:22 AM, <[EMAIL PROTECTED]> wrote:
That would depend on your point of view. As an owner he may not
care if
the cap blows off while the FD is pumping it up during a fire as
mush as
he would if there was no emergency and someone just wanted a test
becaus
Thom,
I'll work on that resume. lol
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-Original Message---
Martin,
With the information you've provided that the replacement was not for
the entire system, or an area easily isolated, I would agree with you,
and with others who've suggested that the only required test is at
system pressure.
As for the contract argument I would suggest that unless th
P.S. Because the system was taken out of service to replace the heads, it
must be "Re-activated" (Generally follow same guidelines as for
"Activation".)
Also if you want to be the "DEVIL'S" Advocate, you must first apply in
person, with a fire proof resume. (If selected you'll have to supply y
Thanks Roland,
I've never fought a fire in my life, so my experience there is gained here
on the forum. Well, no experience except maybe for a few times that I
started a fire accidentally as a kid when I was experimenting with matches,
gasoline, and ants! Anyway, I do have a call into the AHJ, st
In Mil Speak, that means when you initially turn the system on or
"Pressurize" the piping.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: <[EMAIL PROTECTED]>
To:
Sent: Thursday, March 08,
What's the definition of "activating", sprinkler discharge such as
during a fire scenario as opposed to shutting one down for service and
placing it back into service? I can completely understand the
de-energization of critical equipment in a sprinkler discharge scenario
as triggered by the wate
That would depend on your point of view. As an owner he may not care if
the cap blows off while the FD is pumping it up during a fire as mush as
he would if there was no emergency and someone just wanted a test
because they wanted to see what happens to the system.
Craig L. Prahl, CET
Fire Pro
7+2 not 7 total. (9 Total)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Reed Roisum" <[EMAIL PROTECTED]>
To:
Sent: Thursday, March 08, 2007 10:47 AM
Subject: Calculating Attic Heads
I'm concerned about the undertone of the discussions. That is, hydrostatic
testing of existing systems will lead to unpredictable results (things
leaking and coming apart).
If this is the case, then we may have many very fragile systems out there
that shouldn't be in service in the first place.
Well if the PO was for the replacement of heads and the labor to perform
such, then anything beyond that should be handled as a change order.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
IF YOU ARE UNDER THE GUIDANCE OF THE UFC 3-600-01, (adopted by the Dept. of
the Airforce April 2003) take heart!
6-8.1.1 Automatic sprinkler protection, Requires all power to be
disconnected from and sensitive electronic equipment when activating a fire
sprinkler system. (If your facility is "
Does anyone use valve seals during inspections? We use seals similar to
those used on fire extinguishers, but they are not the best. If you take
your time, you can take them off without breaking the seal. If you use
these, where do you get them? Thanks.
Joseph C. Stough CET, CFPS
Tilley Fire E
Because this building is a US Air Force building, I don't think it
will go to a code appeals process, but I can always ask.
We make a quote to change the heads and they issued a purchase order
for the heads and labor. There is no contract language that I can
rely on in this case. Their purch
Has anyone thought to call Tyco? Maybe they have dealt with this exact
issue before - probably many times?
Terri Simmons Leyton
PROTECTION DESIGN & CONSULTING
voice: 858.751.2930
fax: 858.751.2933
cell: 619.871.8450
-Original Message-
From: Jim Kettler [mailto:[EMAIL PROTECTED]
We call these folks "inventors" and they generally give us AHJ-types a bad
reputation. I struggle to get folks to comply with the minimum standards,
let alone invent new requirements!
I think the technical code issues have been well addressed. My only
recommendation to add - avoid turning this int
If water comes out of the sprinkler fittings, then it's your water. If
water comes out anywhere else, it's their water.
Wouldn't this be a fair way to approach the testing?
Bill Brooks
Pittsburgh, PA
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Roland
H
well let the boys that put the wet stuff on the hot stuff address it
but I suspect they pull hose from outside for the ground floor.
I would think the intermediate connection at the first landing is for
the second floor.
Maybe Steve will comment on if the TC has talked about the first floor
If you haven' t already, I would suggest a call to your local AHJ.
Typically firefighting operations would have crews connect at the floor
below; preferably at the intermediate landing below so not to bungle up
access at the floor below. Depending upon the height of the intermediate
landings, the l
The couple of intermediate-landing standpipes I've installed, I put a FDV on
the lowest floor landing as well.
Is this a manual standpipe?
Tom
Go Red Sox!
Roland,
I can understand that, but at the first intermediate set of landings they
will need to go down to reach the first level.
Bob Knigh
I agree with George! How many customers do you have that don't want to
spend the money to proactively repair a system, but call you immediately if
there is a leak, and tell you it is your fault. Unfortunately, even if the
customer likes you and tells you it's not your fault, their insurance
comp
Roland,
I can understand that, but at the first intermediate set of landings they
will need to go down to reach the first level.
Bob Knight
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, March 08, 2007 11:26 AM
To: sprinkle
My understanding is that they thread UP the stairs. Being below the
fire is so much better than being above it.
Roland
On Mar 8, 2007, at 10:04 AM, Bob Knight wrote:
I have a parking garage with a dry manual standpipe. The south
tower is cut
and dry with the standpipe hose valves at each
That is true and thank goodness there are no vindictive consequences
when pointing that out.
Best to give the dog a bone if it will shut them up but if the dog
wants your whole leg, THEN fight about it.
Roland
On Mar 8, 2007, at 7:28 AM, Chris Cahill wrote:
They cannot ask for whatever
In order to omit from the calculations such small rooms (with
light fuel loads as already discussed but poorly defined), you must
have a remote area with a minimum size from Figure 11.2.3.1.1 (ie
1500 sf for LH & OH) plus any increases. IT identifies 30% for dry
pipe but ceiling slope wo
What does your contract specifically define as the scope of your work?
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg
I have a parking garage with a dry manual standpipe. The south tower is cut
and dry with the standpipe hose valves at each intermediate landing. The
north tower, on the other hand, is confusing me. Rather than a single
intermediate landing, there are two intermediate landings. I am planning on
Hi Group,
A little more information about the building. It is on an Air Force
site and the Fire Chief, who is the AHJ, is requiring the hydrostatic
test after the Omega heads were replaced. The fire sprinkler head
replacement did not emcompass the entire building because there are
mixed hea
I am reviewing a dry system attic layout using Tyco's Single Directional
(SD) and Back to Back (BB) attic heads. The attic narrows at the remote
area so that the peak goes from an attic peak (12/4 slope)with roof on
each side, to a roof only on one side of the peak. (sorry for the poor
description
Thank you my thoughts exactly concerning the rooms. I welcome any more
comments, but extend thanks to all.
Kathryn
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jarrod
Poorman
Sent: Thursday, March 08, 2007 9:51 AM
To: sprinklerforum@firesprinkler.org
Viking just released one for up to 14'x14' and rated for QR in OH
applications.
Jarrod Poorman
Sr. Fire Protection Design Technician
Global Fire Engineering
www.global-fire.com
Office (941)-758-2551
Fax (941)-739-6383
Chad Burnett wrote:
Does anyone know if there is an Extended Coverage Head
Does anyone know if there is an Extended Coverage Head that has a QR rating
in and OH applications?
Chad Burnett
Fire Safe Systems
From: "Travis Mack" <[EMAIL PROTECTED]>
Reply-To: sprinklerforum@firesprinkler.org
To:
Subject: RE: Extended Cov. Hds Calc Area
Date: Thu, 8 Mar 2007 09:41:58 -0
If you omit the sprinkler heads allowed in 14.4.4.4.2, you cannot use
the design area reduction. You have to calc to 1500 sqft even if QR
heads are used. If you have the handbook, it goes into further
explanation.
In addition, 14.4.4.4.2 applies to small the rooms with small fuel
loads. O
Kathryn:
The EC-11 are not QR in OH applications. They are SR. Therefore, the QR
reduction does not apply.
As far as:
"Ok I need to add one more question to the omission of these three rooms per
14.4.4.4.2 2002 edition, it states 'closets, washrooms, & similar small
compartments requiring onl
Of course whichever is greater the 900 sq ft or 5 heads...
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kathryn Tyler
Sent: Thursday, March 08, 2007 9:40 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Extended Cov. Hds Calc Area
EXCELLENT!!! Bri
EXCELLENT!!! Brian - it sure would qualify, Thank you very much I did not
even consider that, it will allow ext. cov to be reduced also.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, March 08, 2007 9:32 AM
To: sprinklerforum
Ok I need to add one more question to the omission of these three rooms per
14.4.4.4.2 2002 edition, it states 'closets, washrooms, & similar small
compartments requiring only one head' --- The rooms are a toilet, break room
and an office - I am willing to allow the omission of using the toilet but
Just to be safe on the 1500 sq.ft., is area reduction applicable?
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-Original Message-
From: [EMAIL PROTECTED
Anyone else with different or the same thoughts as Steve?
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kathryn Tyler
Sent: Thursday, March 08, 2007 9:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Extended Cov. Hds Calc Area
The 5 sprinklers
The 5 sprinklers are not the greater, so the 1500 sq. ft. is having to be
used. So include those rooms, I thought that would be true, they are not
demising walls. Thank u
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Thursday, March
I'm pretty sure the language (and intent) of NFPA 13 and manufacturer's
listings of these types of sprinklers is that you calculate 5 sprinklers
minimum, or the area/density method whichever is greater. So if you have
standard sprinklers in compartments that are not fire or area-separated from
Good Morning Forum, I am currently reviewing a project which is
utilizing the Tyco EC-11 extended coverage pendent heads. I have rarely
used them and could use your great input.
My question is:
The calculation area is a kitchen and in the center of the kitchen are
three rooms, toilet,offices (
There is nothing on the drawings that would be construed as a roof
deck. There could be some walkways to service RTUs and the elevator
rood, but that is about it.
At 09:12 AM 3/8/2007, you wrote:
Certainly, if the roof has no "roof decks" designed for occupancy then
the roof is not considered
Hey Ken,
I see your point, but unless you have a control valve at each "new portion"
(each of the 200 spkr)of the sprinkler system, I would say it can't be
isolated. Hydrostatically test the reducer and the head???
The handbook provides the following commentary text...
"The TC of Spkr System Ins
Ken,
If the 200 sprinklers represented the entire system, or an area which
could be isolated from the rest of the system/building, wouldn't
16.2.1.5 support the requirement the AHJ has made?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED]
NO! NO! NO! NO! NO!
The AHJ (Fire Marshal)is a law enforcement officer just like a police
officer. States will vary a bit as to the form of legalities but if you
have the written law on your side you are covered. Now you might have to
exercise your rights in either the appeals system or the cour
All of these are defined terms in the code(s) ... roof, basement, etc. Try
this for a roof - can the space be sold or leased? If so, it's a floor.
Steve L.
-Original Message-
From: R Richardson [mailto:[EMAIL PROTECTED]
Sent: Thursday, March 08, 2007 6:13 AM
To: sprinklerforum@firesp
Make sure you get a release of liability for any and all damage that may
result from any system failure. The liability when testing older
systems can be huge as you have no idea of what has been done to it over
the years or the quality of the original installation. I had been
through this and a c
I'd be happy to include some monies for the replacement of failed pipe and
fittings- IF the Owner will accept liability for property damage and BI and
consequential damages. Heck $5 and 15 minutes to replace a 4" grooved
Coupling ain't much compared to the damage that 700 GPM coming out of it can
d
It may not be a matter of arguing with the AHJ as they can ask for the test
if they wish. You need to meet with them (include the building owner) to
discuss and show him the minimum NFPA requirements.
If the AHJ is still adamant about the hydro test, then you need to prepare a
proposal to the b
>
> We argue that replacement of the heads do not require this 20 year old
system to be hydro >tested. We point out that the system was not modified
and to subject an old system to these >pressures could cause a failure of
its piping.
If subjecting a 20 year old system to a 200 pound hydro test
Certainly, if the roof has no "roof decks" designed for occupancy then
the roof is not considered an occupied floor. If there are roof decks
good chance the answer is yes. We have a local ammendment allowing
small roof decks (less than 50 ocupants) to be provided without
considering it an occupie
Once again, I know this was posted a few weeks ago, but does anyone have
8 extra 2" domestic shut off valves? Our supplier had promised us the
remaining 8 we have outstanding on projects but alas, the 8 that were in
stock have mysteriously disappeared Please contact me off forum if
you can be
>Is there any formal opinions from NFPA that offers guidance on this issue?
Martin,
Read NFPA 13 '02 edition Section 16.2.1.6. The system would not have to be
tested in excess of normal system pressure.
You may also want to check the forum archives. Someone posed this question
not long ago c
Hello list,
We have just finished replaced Omega heads in a buildiing (200 of them) and the
AHJ wants the sprinkler system hydrostatic tested.
We argue that replacement of the heads do not require this 20 year old system
to be hydro tested. We point out that the system was not modified and t
Thanks for the input.
I can not find the reference in 101 that requires a water flow detector on
each floor for a non high rise building.
Thanks,
Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
-Original Message-
From: [EMAI
Here are a couple of replies from the alarm side:
Under the Florida fire prevention which also references 101, it would
require only a flow switch per floor . It would not require A/V devices
in the tenant spaces , only a flow bell and probably remote station
monitoring with a pull station and smo
This may be more picking of nits, but I'm trying to anticipate all
the things that could be thrown at me. The definition uses the phrase
"occupied floors". If a stair tower extends to provide roof access,
does the top landing, which opens out onto the roof constitute an
"occupied floor"?
The
If you are looking at future occupancy, then what do you design to?
What if they put plastic party trays in the racks? It's a tough call.
The owner has to take responsibility (shudder) for providing accurate
information on the building occupancy. If it changes, then it's the
owners responsibili