RE: [EXTERNAL] RE: Sprinklers next to Diffusers

2018-11-09 Thread Kyle . Montgomery
Depends on how you read that table (6.2.5.1). The way I read it, says that you can only use ordinary temp heads if your maximum ceiling temperature is 100 degrees or less. And you can only use intermediate temperature heads if your maximum ceiling temperature is 150 degrees or less. But it doe

RE: Sprinklers next to Diffusers

2018-11-08 Thread Kyle . Montgomery
What Steve said. Generally, my experience has been that if they have a heat pump, max outlet temperature will be less than 100 degrees. But if they have a furnace, there is a good chance it will be higher. Mechanical designer/contractor should be able to answer the question. -Kyle M From: Spr

RE: Main Relief Valve for Diesel Driven Fire Pump

2018-11-05 Thread Kyle . Montgomery
Yes. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Hairfield Sent: Monday, November 5, 2018 10:52 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Main Relief Valve for Diesel Driven Fire Pump Has anyone ever installed a main reli

RE: [EXTERNAL] Single Preaction System

2018-11-01 Thread Kyle . Montgomery
I would think that QR is OK but that C-Factor should still be reduced (100). What does the rest of the forum say? -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bob Knight Sent: Thursday, November 1, 2018 3:35 PM To: sprinklerforum@lists.firesp

RE: [EXTERNAL] Single Preaction System

2018-11-01 Thread Kyle . Montgomery
See 11.2.3.2.5 and A.11.2.3.2.5. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kyle.Montgomery Sent: Thursday, November 1, 2018 3:19 PM To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] Single Preaction S

RE: [EXTERNAL] Single Preaction System

2018-11-01 Thread Kyle . Montgomery
One of the biggest impacts is that calculating as a dry system means you have to increase remote area size by 30%, but you don't have to do that if you can calculate as wet. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bob Knight Sent: Thurs

RE: [EXTERNAL] Re: Combustible Concealed Space

2018-10-23 Thread Kyle . Montgomery
I still need to verify, but it looks like it’s going to have a limited-combustible facing that is stapled in place. For the sake of this argument, let’s assume that is the case. So, it would be most similar to Figure A.8.15.1.2.17, with the following differences: 1. It’s a steel bar jois

Combustible Concealed Space

2018-10-23 Thread Kyle . Montgomery
I'm looking at a building with steel bar joists with a wood nailer and plywood deck. The building will have a drop ceiling, and of course have pendent sprinklers protecting the area below the ceiling. If there is insulation at the deck that covers the deck and wood nailers, do I need upright

RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

2018-10-09 Thread Kyle . Montgomery
but I haven't found anything in NFPA 13 outside of the ESFR section. It sure seems like if it's appropriate for ESFR heads (arguably the most finicky with regard to spacing/obstructions) that the same spacing should be OK for standard spray sprinklers. Kyle Montgomery [cid:image001.gif@

RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

2018-10-09 Thread Kyle . Montgomery
ts) would actually be deficient as a result? I'm thinking about taking this to the AHJ to see if they would allow it, but I don't want to suggest doing it if there is good reason to believe that it is a "bad fire protection practice". I appreciate the input. Kyle Montgom

RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

2018-10-08 Thread Kyle . Montgomery
to suggest doing it if there is good reason to believe that it is a "bad fire protection practice". I appreciate the input. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell

Converting from ESFR to CMDA - Spacing Issues

2018-10-08 Thread Kyle . Montgomery
M Global allows for this, but I haven't found anything in NFPA 13 outside of the ESFR section. It sure seems like if it's appropriate for ESFR heads (arguably the most finicky with regard to spacing/obstructions) that the same spacing should be OK for standard spray sprinklers. Kyle

RE: [EXTERNAL] RE: Material for Lateral Bracing

2018-10-02 Thread Kyle . Montgomery
Tolco has the Figure 4LA which goes up to 12” (FM-Approved). It’s basically a pipe clamp with a built-in attachment to the brace pipe. To answer your question, I think that the components of the assembly have to be listed for use as a seismic brace. So I don’t think you can just grab any 10” pi

RE: Fire sprinklers in harsh coastal environments

2018-10-02 Thread Kyle . Montgomery
Those are pretty expensive though, aren’t they? If you look at the sprinkler cut sheets from Reliable (and others) they generally list the White Polyester heads as “corrosion resistant” and we’ve used those. I don’t think the white polys cost that much more than your standard sprinkler. We’ve u

RE: [EXTERNAL] RE: Sprinkler heads popping off randomly

2018-09-14 Thread Kyle Montgomery
2) 759-5556 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kyle Montgomery Sent: Thursday, September 13, 2018 9:44 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: Re: [EXTERNAL] RE: Sprinkler h

RE: [EXTERNAL] RE: Sprinkler heads popping off randomly

2018-09-14 Thread Kyle Montgomery
water loss? Less than all the engineering I’ve proposed. I get to see the results of piece-meal far too often. Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kyle Montgomery Sent: Thursday

Re: [EXTERNAL] RE: Sprinkler heads popping off randomly

2018-09-13 Thread Kyle Montgomery
Pressure relief valves are “conceivably a waste of money”... coming from the guy that suggested the forensic metallurgist. How much will the forensic metallurgist charge Larry to tell him it’s time to replace his 50-plus year old heads? Sent from my iPhone On Sep 13, 2018, at 6:02 PM, Scott Fu

RE: Hose Connections - Main Stair Landings vs. Intermediate Landings

2018-09-13 Thread Kyle Montgomery
Your statement seems to contradict itself. You say that they are essentially prepared for multiple options, but that we (the fire protection design community) should be forced to comply with the "flavor of the week" that the current fire marshal prefers. As was stated previously, there are ofte

RE: Horizontal Automatic Standpipe Demand

2018-09-07 Thread Kyle Montgomery
Which code section requires automatic standpipes for detention facilities? How long has that been in the code? -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reed A. Roisum, SET Sent: Wednesday, September 5, 2018 5:38 PM To: sprinklerforum@list

Help with Storage Criteria [17.2.1.2.1(F)]

2018-02-01 Thread Kyle . Montgomery
I see the same language in quite a few places in chapter 17, but I’m looking specifically at Figure 17.2.1.2.1(f). The criteria is for “storage 25 ft in height with 5 ft to 10 ft clearance to ceiling”. So that leads me to believe the ceiling could be up to 35 feet… is that right? The language i

RE: [EXTERNAL] RE: FDC & Pump

2018-01-31 Thread Kyle . Montgomery
I disagree. From NFPA 13, 2016 edition: 8.17.2.4.3 For multiple systems, the fire department connection shall be connected between the supply control valve and the system control valves. Wouldn’t that be on the riser manifold? The handbook even goes on to explain why this would be the preferabl

RE: [EXTERNAL] RE: Conveyors

2018-01-25 Thread Kyle . Montgomery
8.5.5 contains GENERAL requirements. Individual sprinkler types (such as ESFR) may have specific requirements, as addressed in section 8.6 thru 8.13. The handbook has commentary that explains this pretty well. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]

RE: [EXTERNAL] RE: Conveyors

2018-01-25 Thread Kyle . Montgomery
While I agree with your theory (I don't feel sprinklers are necessary in this scenario), the NFPA 13 code requirements for continuous obstructions don't seem to have a limit for how far the obstruction is below the sprinkler. If it is 2 ft wide, it should be located 2 ft HORIZONTALLY from the sp

RE: Conveyors

2018-01-25 Thread Kyle . Montgomery
It's an ESFR system. ESFR has more restrictions than just applying 8.5.5 rules. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Joe Delvo Sent: Thursday, January 25, 2018 8:02 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: Conveyors

RE: [EXTERNAL] ESFR Stuff

2018-01-25 Thread Kyle . Montgomery
We dealt with this recently where the argument was how to define “adjacent” sprinklers and whether a mezzanine some 10-plus feet below the ESFR system should be considered adjacent. I’m not sure if there was a consensus. But that was a concern because the heads under the mezzanine were going to

RE: [EXTERNAL] Calculation of sprinklers under soffits

2018-01-25 Thread Kyle . Montgomery
In 2013 they added section 8.6.5.1.2(4) which basically says (I’m paraphrasing) that you don’t need sprinkler protection under soffits less than 24” wide, as long as the sprinkler at the higher ceiling is spaced close enough to the wall (measure to the wall and not the face of the soffit). If yo

RE: [EXTERNAL] Calculation of sprinklers under soffits

2018-01-24 Thread Kyle . Montgomery
Are you saying that the soffits extend/project 18” from the wall? If so, are sprinklers actually required beneath the soffits? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: Wednesday, January 24, 2018 3:48 PM To: Sprinklerforum Subje

RE: Conveyors

2018-01-24 Thread Kyle . Montgomery
[Tangent Alert] With regard to common sense, for most of these large fulfillment centers their entire livelihood is based upon knowing exactly where every package/product is at all times. What is the likelihood that they would just throw a few packages under the conveyor, or let debris accumulat

RE: [EXTERNAL] RE: Deflector Distance for Sprinklers in Skylights

2018-01-05 Thread Kyle . Montgomery
Are the skylights less than 32 square feet? If so, does 8.5.7.1.1 apply? If so, there’s your answer… But I’m not sure if it does since 8.5.7.1.1 is a “subtext” to 8.5.7.1, which is specific to situations where the skylights are less than 32 square feet AND separated by at least 10 feet. But 8.5

RE: ESFR Calc Question - Obstructions

2018-01-05 Thread Kyle . Montgomery
That's what we've been defaulting to. But what if I don't want to use the same pipe size to the head under the obstruction? Most of the time I'm dealing with a duct/diffuser for an evap cooler that only requires a single sprinkler. I think we can agree that providing 3" pipe to a single ESFR sp

ESFR Calc Question - Obstructions

2018-01-05 Thread Kyle . Montgomery
Way back in the Dark Ages of Sprinkler Design (2010) when you had to add ESFR sprinklers under obstructions you were required to add the discharge for up to 2 of them to your overhead calc, thus flowing 14 (12+2) sprinklers. In 2013, the section requiring the two additional heads was removed (or

ESFR Area and Office Area Separated by Partial-Height Wall

2017-12-13 Thread Kyle . Montgomery
I’m looking at a project that is a spec building with office areas at the front of the building and shop/storage in the rear. The office areas are separated from the shop areas by a partial-height wall (building is almost 30 feet tall, wall stops at 12’-0” A.F.F.). The shop/storage areas are spe

RE: [EXTERNAL] Re: Protection under bleachers in a Gymnasium

2017-12-13 Thread Kyle . Montgomery
Bringing sexy back to the NFPA handbook. Just one more thing Roland Huggins and Justin Timberlake have in common. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Nick Maneen Sent: Tuesday, December 12, 2017 6:10 PM To: sprinklerforum@lists.firesprinkler

RE: [EXTERNAL] Re: Dry automatic standpipe without a pump

2017-12-08 Thread Kyle . Montgomery
Steve, Thanks for the detail on that, but I must not have been very clear with my point. I understand how a manual wet/dry standpipe works. My question was why do they connect to an automatic water supply, via the dry pipe valve, that is not capable of providing the required pressure? Why not j

RE: [EXTERNAL] Re: Dry automatic standpipe without a pump

2017-12-08 Thread Kyle . Montgomery
Yeah, but what good is it to connect to a water supply that can’t supply the pressure you need? The only thing that really makes sense is that they are doing it for supervisory purposes; i.e. someone breaks a pipe or opens a valve, water starts pouring out and an alarm sounds. But couldn’t you a

RE: Nebraska Edition of NFPA 13

2017-12-07 Thread Kyle . Montgomery
Omaha is on 2007 edition, according to a source I trust that lives and works there. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reed A. Roisum, SET Sent: Thursday, December 07, 2017 9:31 AM To: sprinklerforum@lists.firesprinkler.org Subject:

RE: [EXTERNAL] Re: Tablets for survey?

2017-12-06 Thread Kyle . Montgomery
Our construction manager uses a tablet with Bluebeam (PDF editor) for this purpose and he really likes it. I haven’t tried it yet myself. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: Wednesday, December 06, 2017 4:04 PM To: S

High-Rise with Secondary Water Supply

2017-12-06 Thread Kyle . Montgomery
the backflow prevention device? We’ve been asked to provide galvanized pipe in similar scenarios before, but it was suggested that that might not be AWWA-compliant. Thanks for your input. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix

RE: Dry automatic standpipe without a pump

2017-12-05 Thread Kyle . Montgomery
This actually does make a lot of sense. Maybe that is even what the City of Orlando intended when they wrote the code. Couldn’t you just have supervisory air for that though, without actually being connected to a water supply with a dry pipe valve? -Kyle M From: Sprinklerforum [mailto:sprinkle

RE: [EXTERNAL] RE: Dry automatic standpipe without a pump

2017-12-05 Thread Kyle . Montgomery
The definition of Automatic Dry Standpipe says that. But then Sean is left with a system that doesn't actually fit any definition (literally, if not practically). But, I agree, it should go without saying that you don't need a definition for something that makes no sense to do in the first plac

RE: [EXTERNAL] RE: Dry automatic standpipe without a pump

2017-12-05 Thread Kyle . Montgomery
Here's what's muddying the waters: NFPA 14 - 3.3.17.5 Manual Dry Standpipe System. A standpipe system with NO PERMANENTLY ATTACHED WATER SUPPLY that relies exclusively on the fire department connection to supply the system demand. I think that most of us can agree that what the Sean is dealing

RE: [EXTERNAL] Re: Saw-Tooth Ceilings

2017-12-05 Thread Kyle . Montgomery
You guys are making a good case... I'm just having a hard time with it because it's different than what I've been doing for 10 years. But as a contractor, it would definitely be helpful if I was wrong in this instance (i.e. save some money). I wish some of the "Big Wigs" on this site would chim

RE: [EXTERNAL] Re: Saw-Tooth Ceilings

2017-12-03 Thread Kyle . Montgomery
That is true. (See 23.4.4.6.5) Thanks for pointing that out. But that does not mean you can ignore the obstruction when determining the required discharge, right? That was the premise of the original question. I’ll amend my previous statement to say the area used for determining minimum dischar

RE: [EXTERNAL] Re: Saw-Tooth Ceilings

2017-12-03 Thread Kyle . Montgomery
I disagree, Brad. Whatever distances you use to determine S x L for spacing the sprinklers, the same distances must be used to determine area of coverage for hydraulic calculations. (NOTE: There are a few exceptions, such as when using the 'Small Room Rule'). I think that NFPA 13 spells it ou

RE: [EXTERNAL] Re: Quick swaybrace calc question

2017-11-27 Thread Kyle . Montgomery
Dynaflow, etc.) that you either need to use the Sch 5 table or get the data from the manufacturer. In my experience, it is worth it to use the manufacturer's data because it is way more robust than Sch 5. Kyle Montgomery   Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024

RE: [EXTERNAL] Interesting issue .. residential sprinklers ..

2017-11-21 Thread Kyle . Montgomery
True. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin Sent: Tuesday, November 21, 2017 7:46 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] Interesting issue .. residential sprinklers .. Yes. That’s an option as well. I h

RE: [EXTERNAL] Education Requirements for Fire Protection Industry

2017-11-21 Thread Kyle . Montgomery
Yes, fire sprinkler contractors value education. As far as NICET certification… kind of. It’s necessary in some jurisdictions to have at least a NICET III stamp plans. And when it is time to hire someone new, knowing they are NICET certified at the very least gets a foot in the door. But if I a

RE: [EXTERNAL] Interesting issue .. residential sprinklers ..

2017-11-21 Thread Kyle . Montgomery
Residential sprinklers are “permitted” in dwelling units, not “required”, right? Couldn’t you use any one of a number of commercial QR extended coverage sprinklers? That might mess you up if you are trying to do a 4-sprinklers residential calc… or it could help because you could get a larger K-

RE: ESFR In A Ceiling

2017-11-16 Thread Kyle . Montgomery
Chris, See below. Someone has obviously hacked your account. :) From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Thursday, November 16, 2017 9:54 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: ESFR In A

RE: [EXTERNAL] RE: lag bolts

2017-10-25 Thread Kyle . Montgomery
Why would you do that instead of using a thru-bolt? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Rocci Cetani 3 Sent: Wednesday, October 25, 2017 10:51 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: lag bolts I did think about t

RE: [EXTERNAL] Re: Small Hose Connections

2017-10-24 Thread Kyle . Montgomery
Yeah. The reason I got here was because I asked the AHJ if they required them, and he referred me to 8.17.5. I wanted to make sure there wasn’t another code requirement somewhere that dictated when they are required before I followed up with him. Thanks all. Kyle Montgomery [cid:image001.gif

RE: [EXTERNAL] RE: Underground Main

2017-10-24 Thread Kyle . Montgomery
h I think is what leads to all these different strategies as to how to "calc the underground". Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom...@aerofi

Small Hose Connections

2017-10-24 Thread Kyle . Montgomery
ty having jurisdiction in accordance with 8.17.5 for first-aid fire-fighting and overhaul operations. Is there a code section somewhere that tells me if/when the small hose connections are required? Or is it solely up to the AHJ to determine if he wants them or not? Kyle Montgomery [cid:image001.gi

RE: [EXTERNAL] RE: Underground Main

2017-10-24 Thread Kyle . Montgomery
to size the underground, which I think is what leads to all these different strategies as to how to "calc the underground". Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 60

RE: NYC Standpipe

2017-10-24 Thread Kyle . Montgomery
I would think 4" would be allowable for the shorter standpipes, but I've never worked in NYC so my thoughts probably aren't worth much. You are going to run calcs to prove that 4" would work hydraulically, right? Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Au

RE: Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread Kyle . Montgomery
ge sprinkler, but it's about double the cost of a normal 8.0K sprinkler. The outside edge of the mezzanine is formed by beams, so there is kind of a draft stop; but there is a corrugated deck with gaps above the beam for heat to escape through, so it isn't really an effective draf

RE: Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread Kyle . Montgomery
anyone knew of another option. All comments are appreciated. Thanks guys. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com>

Sprinkler Heads Under Mezzanine In ESFR Warehouse

2017-10-18 Thread Kyle . Montgomery
mezzanine is formed by beams, so there is kind of a draft stop; but there is a corrugated deck with gaps above the beam for heat to escape through, so it isn’t really an effective draft stop. Thanks guys. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N

RE: [EXTERNAL] RE: RE: Car Wash Station

2017-10-12 Thread Kyle . Montgomery
Architects/engineers often ask for "corrosion resistant" heads in locker rooms with showers or in exterior locations that are exposed to ocean air, for example. I'm not sure if there is a real, tangible corrosion concern in a car wash, but it's an easy safeguard to use white-poly heads.

RE: [EXTERNAL] RE: Car Wash Station

2017-10-12 Thread Kyle . Montgomery
Corrosion. I'm not sure if that is really an issue or not, but I would probably use white poly heads. Cost difference is basically negligible. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday,

RE: [EXTERNAL] Re: Soffit Along a Wall

2017-10-12 Thread Kyle . Montgomery
Agreed. "Sprinklers shall be arranged to comply with ONE of the following arrangements:" If you comply with the first one (beam rule) you don't have to any further. -Kyle M -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of bcas

RE: Attic Design, Using BB1 & AP Sprinklers

2017-10-11 Thread Kyle . Montgomery
I think that is a pretty solid assumption. I just had a seminar about attic sprinklers and that is exactly what happened in the tests they showed. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark Sornsin [FAR] Sent: Wednesday, October 11, 20

Obstructed Construction Clarification

2017-10-09 Thread Kyle . Montgomery
Sorry in advance if this has already been addressed ad nauseam. It’s pretty common to see steel beam construction with concrete over a corrugated metal deck (see Exhibit 3.32 in the 2016 handbook for a picture). This kind of construction can fall into three categories (correct me if I’m wrong):

RE: [EXTERNAL] Calcs and tenant improvements

2017-10-06 Thread Kyle . Montgomery
Travis, Are you seeing this in AZ, or are you doing a lot of work in other states? It seems like the AHJs we deal with in the valley are usually pretty lax on requiring calcs for T.I.s. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Ma

RE: Pipe Schedule System

2017-10-06 Thread Kyle . Montgomery
Probably semantics, but if the water supply has improved enough that a calculation now works, then it is no longer a “pipe schedule” system. It is now a “hydraulically calculated” system. So you could throw that 20 psi stipulation out the window. I doubt you’ll have a working calculation where

RE: [EXTERNAL] dry systems in parking garages exception

2017-10-02 Thread Kyle . Montgomery
Are the 4 floors combined less than 52,000 sq. ft.? Or are they just individually less than 52,000 sq. ft.? Are you pretty confident you can meet the water delivery times with all four floors on one valve? Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605

RE: NFPA 13 8.17.5.2.2(1)

2017-08-31 Thread Kyle . Montgomery
The figures that are shown for this section [A.8.17.5.2.2(a) and (b)] show your classic combination standpipe, though. That's what is confusing me. I've always thought of "inside hose" or "hose connections supplied by a sprinkler system" as being differentiated from standpipe connections because

RE: NFPA 13 8.17.5.2.2(1)

2017-08-31 Thread Kyle . Montgomery
I read the handbook commentary for 8.17.5.2, and now I'm confused again: "When either one of the hose connections described in 8.17.5 is provided, the flow rates need only be added to the sprinkler system at the design pressure available at the point of connection to the sprinkler system pipe."

RE: NFPA 13 8.17.5.2.2(1)

2017-08-30 Thread Kyle . Montgomery
This has been my understanding as well. I wonder why more people don't do it this way? I've done it myself one time. But usually am met with a lot of skepticism in the form of "well, if this is acceptable, why doesn't everyone do it that way?" From: Sprinklerforum [mailto:sprinklerforum-boun...

RE: NFPA 13 8.17.5.2.2(1)

2017-08-30 Thread Kyle . Montgomery
I'm wondering why it isn't more common, considering you purchase about half as many PRVs that way. Would you need to flow a hose allowance through that valve as part of you sprinkler calculation? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Le

RE: NFPA 13 8.17.5.2.2(1)

2017-08-30 Thread Kyle . Montgomery
Not to sidetrack this thread... but is the arrangement Colin is describing acceptable? I have never found anything in the code saying it isn't, but I would say that almost every installation I've seen has a separate pressure-reducing hose valve and pressure-reducing system control valve... whic

RE: Hose Valves at Horizontal Exits

2017-08-29 Thread Kyle . Montgomery
Yeah, I was looking in an older version of NFPA 14. That figure in the new version really clears it up. Thanks guys. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom

Hose Valves at Horizontal Exits

2017-08-29 Thread Kyle . Montgomery
required to have two exit stairs (one in each fire area) located within 130 feet of the horizontal exit, reachable from both sides? Or is any one exit stairway within 130 feet of the horizontal exit OK? Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605

RE: [EXTERNAL] Re: Radiant heat panels

2017-08-28 Thread Kyle . Montgomery
And the radiant heaters are typically mounted below the sprinklers, with a “heat shield” that reflects the heat down towards the occupants. This came up recently on an ESFR building (where intermediate temp is the highest we could go) and the mechanical guys weren’t concerned at all about the he

RE: [EXTERNAL] Re: Storage Under Sloped Ceilings

2017-08-23 Thread Kyle . Montgomery
That’s what I was finding. This is what had me wondering: 12.1.2 Ceiling Slope. … unless modified by a specific section in Chapter 12 and Chapters 14 through 20. That sent me on a wild goose chase to find the specific section where it was modified. Thanks, all. -Kyle M From: Sprinklerforum [

Storage Under Sloped Ceilings

2017-08-22 Thread Kyle . Montgomery
I've got an owner that wants to store a Class IV commodity, palletized, solid-piled in a building where the ceiling slope exceeds 2-in-12 and the peak is just over 35 feet. Are there any NFPA 13 protection options that can accommodate this? If he goes with Ordinary Group 2 at the ceiling, then

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-18 Thread Kyle . Montgomery
This statement is the invisible line that separates the engineering firms from the installing contractors. It’s a whole different ball game when you start attaching dollar signs to your safety margins. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Beha

RE: [EXTERNAL] Server Rooms

2017-08-16 Thread Kyle . Montgomery
Well, a server room would be unoccupied the majority of the time, right? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of James Crawford Sent: Wednesday, August 16, 2017 12:20 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Server Rooms

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Then I think you should be able to use the section you are referring to and have a maximum unsupported length of 60”. Is it a welded branch line? That make it a little bit easier sell than if it’s threaded with individual segments. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.fires

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Not true. The "over 100 psi" issue is only a factor when you have pipe above the ceiling feeding sprinklers below a ceiling. If it is an exposed condition with uprights or pendents on the line, then the presence of a pump is not relevant. -Original Message- From: Sprinklerforum [mailto:

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Well, if they are only supplying one head, then “technically” they are an armover, right? Are they attached directly to the main, or on a tee at the top of a riser nipple? -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Dewayne Martinez Sent: F

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Kyle . Montgomery
The CRR (corrosion resistance ratio) is solely based on wall thickness: CRR = (X / Y)^3 Where: X is the thickness of the pipe in question at the first exposed thread OR THINNEST WALL SECTION FOR UNTHREADED PIPE. And Y is the thickness of schedule 40 pipe under the first exposed thread. So if

Building Expansion Joints in NON-seismic Areas

2017-08-09 Thread Kyle . Montgomery
The only reference to expansion joints I can find in NFPA 13 is within section 9.3 "Protection of piping WHERE SUBJECT TO EARTHQUAKES". So, if I'm not in an area that is subject to earthquakes, can I ignore the building expansion joints? Usually I still add a flexible coupling just to be safe, s

Quick-Response Sprinklers in Storage/Extra Hazard

2017-08-07 Thread Kyle . Montgomery
NFPA 13 section 11.2.3.2.2.2 states that QR sprinklers shall not be permitted for use in extra hazard occupancies. Section 12.6.6 states that the use of QR sprinklers shall be permitted when listed for such use. So, if I have a storage occupancy where the appropriate design criteria table dire

RE: Longitudinal Bracing Question

2017-08-01 Thread Kyle . Montgomery
Ryan, I think this is a much more eloquent way of saying what I was trying to say; thank you. I agree that the detail section B was not a good representation. In reality, the geometry of the 4L or 4LA is essentially such that it forces the brace member into the proper axis. Now, do you think t

RE: Longitudinal Bracing Question

2017-08-01 Thread Kyle . Montgomery
Rubbish? Challenge accepted! Of course the “standard” configuration of seismic braces imparts a vertical force on the main. A bunch of sketches would be helpful here, but in lieu of, let me try to describe: In a standard configuration, the brace works in tension and compression to resist the h

RE: Longitudinal Bracing Question

2017-08-01 Thread Kyle . Montgomery
Here is a picture of what I'm talking about (let me know if the picture shows up): It still maintains an appropriate angle from vertical. And it still resists motion "parallel to the axis of the system piping". But in doing so it will impart an additional horizontal load perpendicular to the

RE: Longitudinal Bracing Question

2017-08-01 Thread Kyle . Montgomery
I knew where you were going, Steve, and I agree that this is a good approach. We’ve gone this route in the past, but when you get to the stage of the job where I’m usually involved (closer to construction) and everyone has contracts for construction, it can sometimes be contentious as far as who

RE: Longitudinal Bracing Question

2017-07-27 Thread Kyle . Montgomery
hat. But what size angle iron would we use? I’m sure that a structural engineer could design several viable options, but I’m looking for something that is listed/prescriptive. I’m also interested in hearing what you’ve seen/done that might not be a listed method, just for ideas. Thanks in

RE: Longitudinal Bracing Question

2017-07-27 Thread Kyle . Montgomery
l viable options, but I’m looking for something that is listed/prescriptive. I’m also interested in hearing what you’ve seen/done that might not be a listed method, just for ideas. Thanks in advance for your help. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co.

Longitudinal Bracing Question

2017-07-27 Thread Kyle . Montgomery
tural engineer could design several viable options, but I'm looking for something that is listed/prescriptive. I'm also interested in hearing what you've seen/done that might not be a listed method, just for ideas. Thanks in advance for your help. Kyle Montgomery [cid:image001.gi

RE: ESFR's in Buildings with Concrete Double Tee Construction

2017-07-21 Thread Kyle . Montgomery
have usually been pretty helpful (and reasonable) when it comes to dealing with this kind of stuff. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom...@aerofire.com

RE: Calculation requirement when adding sprinklers

2017-07-18 Thread Kyle . Montgomery
I agree. Unless your fitter really understands sprinkler system hydraulics, your canned answer should probably be that he needs to check with the designer. This can get REALLY tricky if QR reduction has been used or the new area is being really compartmentalized. Kyle Montgomery [cid:image001

RE: Parking Under MTA Tracks

2017-06-29 Thread Kyle . Montgomery
customer? Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com> From: Sprinklerforum [mailto:sprinklerforu

Extended Coverage Sidewall Under Overhead Doors

2017-06-27 Thread Kyle . Montgomery
doors as light hazard in other applications? The doors in question are 16-feet wide and I was hoping to use a ECLH sidewall sprinkler in lieu of an ECOH sidewall or two standard spray sidewalls. Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co. 21605 N. Central

RE: take off before pump

2017-06-22 Thread Kyle . Montgomery
Good point. You could still do it, but you need to check it in such a way that the pump can’t pressurize the low pressure side through the FDC connection. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bruce Verhei Sent: Thursday, June 22, 2017 10:25 AM

<    1   2