RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread BRUCE VERHEI via Sprinklerforum
s.com > 1041 East Butler Road Greenville, South Carolina 29606 > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Tuesday, August 25, 2020 10:29 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: John Denhardt &g

Re: Window Sprinklers

2020-08-25 Thread AKS-Gmail-IMAP via Sprinklerforum
If you are referring to Tyco WS sprinklers, then you do see that it is not listed when there is a horizontal mullion but you also see in its installation details that there is no maximum distance indicated for the “ceiling” to the sprinkler. Yup, go look at. One other aspect to this is that

Re: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Joe Burtell via Sprinklerforum
bs.com > 1041 East Butler Road Greenville, South Carolina 29606 > > -Original Message- > From: Sprinklerforum On > Behalf Of Joe Burtell via Sprinklerforum > Sent: Tuesday, August 25, 2020 10:26 AM > To: å... .... > Cc: Joe Burtell ; > sprinklerforum@list

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On Behalf Of John Denhardt via Sprinklerforum Sent: Tuesday, August 25, 2020 10:29 AM To: sprinklerforum@lists.firesprinkler.org Cc: John Denhardt Subject: [EXTERNAL] Re: Window Sprinklers Agree 100%. Follow

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
Butler Road Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On Behalf Of Joe Burtell via Sprinklerforum Sent: Tuesday, August 25, 2020 10:26 AM To: å... Cc: Joe Burtell ; sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Re: Window Sprinklers Here

Re: Window Sprinklers

2020-08-25 Thread John Denhardt via Sprinklerforum
Agree 100%. Follow the Listing - period. If an architect or an engineer wants to violate the Listing, let them provide direction and assume all liability. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p:

Re: Window Sprinklers

2020-08-25 Thread Joe Burtell via Sprinklerforum
Here is how I see it. All manufacturers prohibit horizontal mullions. My guess is they failed testing when horizontal millions were present. The building code requires the windows to be protected with listed sprinklers. Even if I did put the additional window sprinkler below the horizontal

RE: Window Sprinklers

2020-08-25 Thread Matt Grise via Sprinklerforum
I would ask - what would the lower sprinklers do? It seems like higher level sprinklers would go off first and then prevent the lower ones from operating. As you mentioned, they are not listed for that application. I have had the discussion before: If you want a fire rating, and a window, you

RE: Window sprinklers

2013-02-22 Thread A.P.Silva
Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fairchild, Jack Sent: February 22, 2013 7:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers The ICC pulled the evaluation report based on the code change

RE: Window sprinklers

2013-02-22 Thread bcasterline
Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fairchild, Jack Sent: February 22, 2013 7:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers The ICC pulled the evaluation report based on the code change

RE: Window sprinklers

2013-02-21 Thread Rod DiBona
Pretty sure you do. The mullion acts as a barrier. More than likely if you present the dilemma to the A/E team they change the window. Rod at Rapid -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva

RE: Window sprinklers

2013-02-21 Thread bcasterline
I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona r...@rapidfireinc.com: Pretty sure you do. The mullion acts as a barrier. More than likely if you

RE: Window sprinklers

2013-02-21 Thread Cahill, Christopher
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of bcasterl...@fsc-inc.com Sent: Thursday, February 21, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mullions are considered

Re: Window sprinklers

2013-02-21 Thread Justin Reid
, February 21, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona r

Re: Window sprinklers

2013-02-21 Thread bcasterline
, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona r...@rapidfireinc.com

RE: Window sprinklers

2013-02-21 Thread Russell Carol Gregory
I presume you mean a window with two panes separated by a vertical mullion. By most Codes/Rules: If the sprinkler/drencher is located centred on the mullion then one is OK. If mullion is less then 40mm proud of surface it can be ignored. Otherwise each pane of a window must be sprayed

Re: Window sprinklers

2013-02-21 Thread AKS-Gmail-IMAP
] On Behalf Of bcasterl...@fsc-inc.com Sent: Thursday, February 21, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. Greg McGahan

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
The NRC Canada's IRC has an interesting article on the use of SSP QR heads to protect tempered glass windows, but I don't believe ICC has adopted any of these yet. http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136

RE: WINDOW SPRINKLERS

2010-04-02 Thread John Drucker
@firesprinkler.org Subject: RE: WINDOW SPRINKLERS The NRC Canada's IRC has an interesting article on the use of SSP QR heads to protect tempered glass windows, but I don't believe ICC has adopted any of these yet. http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html Thom McMahon, SET Firetech, Inc

Re: WINDOW SPRINKLERS

2010-04-02 Thread George Medina Jr
. George Medina Jr. -Original Message- From: Greg McGahan g...@livingwaterfp.com To: sprinklerforum@firesprinkler.org Sent: Thu, Apr 1, 2010 7:01 pm Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. I take the word sill iterally when applying

RE: WINDOW SPRINKLERS

2010-04-02 Thread Greg McGahan
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Friday, April 02, 2010 10:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs

RE: WINDOW SPRINKLERS

2010-04-01 Thread Steve Leyton
You're not allowed horizontal mullions or molding. The glazing can be separated by vertical mullions so long as each panel has its own sprinkler, but horizontal bumps are a deal-breaker. Steve Leyton Protection Design Consulting San Diego, CA -Original Message- From:

Re: WINDOW SPRINKLERS

2010-04-01 Thread George Medina Jr
: Thu, Apr 1, 2010 12:22 pm Subject: RE: WINDOW SPRINKLERS You're not allowed horizontal mullions or molding. The glazing can be eparated by vertical mullions so long as each panel has its own sprinkler, but orizontal bumps are a deal-breaker. Steve Leyton rotection Design Consulting an Diego

RE: WINDOW SPRINKLERS

2010-04-01 Thread Robert Thompson
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 2:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½ mullions are vertical and was asking if each panel

RE: WINDOW SPRINKLERS

2010-04-01 Thread Thom McMahon
] On Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 1:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½ mullions are vertical and was asking if each panel required separate sprinklers for them exceeding 1. Thanks, George

RE: WINDOW SPRINKLERS

2010-04-01 Thread John Drucker
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 3:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½ mullions are vertical and was asking if each panel required separate

RE: WINDOW SPRINKLERS

2010-04-01 Thread Steve Leyton
To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS George, The objective is that the entire surface of the glass be wetted. John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ -Original Message

RE: Window sprinklers

2010-03-09 Thread John Drucker
08, 2010 11:47 PM To: sprinklerforum@firesprinkler.org Subject: Re: Window sprinklers In regard to the first question about to WS or not to WS, note that the building code is: On Mar 8, 2010, at 9:59 PM, John Drucker wrote: BETWEEN 4 INCHES AND 12 INCHES (102 MM AND 305 MM) AWAY FROM

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
Only the person that specified the rated wall or alternate means and methods for the glass can answer that. You'll note NFPA 13 doesn't have anything for a contractor to follow, thus this is architect or engineering work to decide how to do it. FWIW I've seen both and am comfortable with SS when

RE: Window sprinklers

2010-03-08 Thread Sal Izzo (TECH- 103)
In answering this question, one must first ask if there is fire resistance rating required to be maintained with this installation. Only listed window sprinklers are tested and listed to provide an actual fire resistance rating for glazing. This is because these sprinklers are tested in

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal Izzo (TECH- 103) Sent: Monday, March 08, 2010 12:06 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers In answering this question, one must

RE: Window sprinklers

2010-03-08 Thread Thom McMahon
To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers In answering this question, one must first ask if there is fire resistance rating required to be maintained with this installation. Only listed window sprinklers are tested and listed to provide an actual fire resistance rating

RE: Window sprinklers

2010-03-08 Thread Thom McMahon
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo Sent: Monday, March 08, 2010 2:12 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Sal, I am not challenging your knowledge or expertise, and while I agree

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Monday, March 08, 2010 1:21 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: Wasn't the whole Atrium glass issue because the walls around an atrium were being

RE: Window sprinklers

2010-03-08 Thread Sal Izzo (TECH- 103)
From: sprinklerforum-boun...@firesprinkler.org [sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo [bcap...@cox.net] Sent: Monday, March 08, 2010 4:11 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Sal, I am not challenging your knowledge

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
@firesprinkler.org Subject: RE: Window sprinklers Bob: Wasn't the whole Atrium glass issue because the walls around an atrium were being treated like exposure protection, not as rated assembly compliance? What I think I heard, and could be wrong, was that SSP/ssu closely spaces were wetting the glass

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
] On Behalf Of Sal Izzo (TECH- 103) Sent: Monday, March 08, 2010 1:42 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: I agree, Bob. My dear friend John Drucker would be disappointed in me for forgetting about the ability of the building code in providing such prescriptive

RE: Window sprinklers

2010-03-08 Thread Tom Duross
Wait. You mean this exterior dry horizontal sidewall head I'm supposed to center over the exterior window connected to the wet system piping in the ceiling might not work the way the engineer drew it? Buy an engineer drew it? It's on the drawring? (my apologies, a sore spot still..) Wong Not

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
, March 08, 2010 4:11 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Wait. You mean this exterior dry horizontal sidewall head I'm supposed to center over the exterior window connected to the wet system piping in the ceiling might not work the way the engineer drew it? Buy

RE: Window sprinklers

2010-03-08 Thread John Drucker
Subject: RE: Window sprinklers Bob: I agree, Bob. My dear friend John Drucker would be disappointed in me for forgetting about the ability of the building code in providing such prescriptive alternatives. My intent was to just make the distinction between a sprinkler actually tested against ASTM

Re: Window sprinklers

2010-03-08 Thread AKS-Gmail-IMAP
In regard to the first question about to WS or not to WS, note that the building code is: On Mar 8, 2010, at 9:59 PM, John Drucker wrote: BETWEEN 4 INCHES AND 12 INCHES (102 MM AND 305 MM) AWAY FROM THE GLASS AND DESIGNED SO THAT THE ENTIRE SURFACE OF THE GLASS IS WET UPON ACTIVATION OF

RE: Window Sprinklers

2009-03-21 Thread Fletcher, Ron
I would say no you can't use them for floor coverage. On the plus side though I don't think you have to worry about cold soldering from the ceiling sprinklers either. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ 85024 -Original Message- From:

RE: Window Sprinklers

2009-03-21 Thread Cliff Whitfield
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron Sent: Saturday, March 21, 2009 8:13 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers I would say no you can't use them for floor coverage. On the plus side though I don't think you

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff Whitfield Sent: Saturday, March 21, 2009 7:20 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers

RE: Window Sprinklers

2009-03-21 Thread Cliff Whitfield
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Saturday, March 21, 2009 12:34 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Also unless the windows extend to the ceiling the widow sprinklers will be placed lower than the ceiling protection

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Thom, That brings up another issue I've been wondering about. I am being required to use these on both sides of the windows. I have not studied the details yet but if the top of the window is at 7' AFF and the ceiling is at 12', how do

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
ICC link to report http://www.icc-es.org/reports/pdf_files/NES/NER516.pdf Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- ___

RE: Window Sprinklers

2008-10-06 Thread Fletcher, Ron
Subject: RE: Window Sprinklers Its important to keep the context of the building code clear. First 2006 IBC Section 704 applies to EXTERIOR WALLS. 2006 IBC 704.12 Opening Protection applies to; WINDOWS in EXTERIOR WALLS REQUIRED to have protected openings in accordance with other sections

RE: Window Sprinklers

2008-10-03 Thread Fletcher, Ron
Thanks man, great information. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... Sent: Friday, October 03, 2008 5:03 AM To: sprinklerforum@firesprinkler.org Subject: Window Sprinklers Pagni, at

RE: Window Sprinklers

2008-10-03 Thread Steve Leyton
That explains a lot about the composition of fire-rated glazing. I don't know what the treatment is that's applied to Fire-Lite or other rated glass but the knock on those products is that they are exorbitantly expensive. It's not as if you can order up pieces of it - you have to purchase

RE: Window Sprinklers

2008-10-03 Thread Justin Reid
In an exposure fire like the one described, it would be the responsibility of the design team to make sure that the fusible link of the sprinkler head is in an area that can sense the exposure threat. NFPA 80A discusses this concept in its appendix. So the glass bulb in the sprinkler head

RE: Window Sprinklers

2008-10-03 Thread Fletcher, Ron
Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Justin Reid Sent: Friday, October 03, 2008 10:17 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers In an exposure fire like the one described, it would be the responsibility

RE: Window Sprinklers

2008-10-03 Thread Chris Cahill
: Friday, October 03, 2008 11:16 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Yes but the building code does not! So I guess where you have no building code your OK. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970

RE: Window Sprinklers

2008-10-03 Thread John Drucker
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers You DO NOT need building code permission use these heads in an unsprinklered building. They comply with the building code. The building code requires a rated wall. We prove ratings through listing agencies performing tests. WS heads passed

RE: Window Sprinklers

2008-10-02 Thread Russell
10 years is new when you've been in this trade for 30 yrs. wouldn't you think? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] ___ Sprinklerforum mailing list

RE: Window Sprinklers

2008-10-02 Thread Fletcher, Ron
, October 02, 2008 5:12 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 10 years is new when you've been in this trade for 30 yrs. wouldn't you think? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED

RE: Window Sprinklers

2008-10-02 Thread Russell
] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Thursday, October 02, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers ToMAYto, toMAHto - my point only being that it's not as if these sprinklers just showed up with the I-codes. Quell is newer, EC storage

RE: Window Sprinklers

2008-10-01 Thread Bill Minkel
Ah, Gotcha Bill Minkel, Designer Dallas, TX -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Tuesday, September 30, 2008 3:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Of course it's MORE than adequate

RE: Window Sprinklers

2008-10-01 Thread bill . brooks
, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell Original Message Subject: RE: Window Sprinklers From: Bill Minkel [EMAIL PROTECTED] Date: Wed, October 01, 2008 9:27 am To: sprinklerforum

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
Design Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, October 01, 2008 6:43 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a guess but I think the window damage

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
@firesprinkler.org Subject: RE: Window Sprinklers The window sprinkler was tested using the exact same criteria as is used to establish any other rated assembly. A test fire is built on one side of the subject and burned for the duration of the rating and then there's a steady-stream hose test

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
Yes. Steve Leyton Protection Design Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 8:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers So the test

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Same as for any rated wall or partition. It can't do it's job if it's not intact. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491

RE: Window Sprinklers

2008-10-01 Thread Craig.Prahl
, Ron Sent: Wednesday, October 01, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers And nobody thinks that might be a problem? I have installed these heads four feet below a ceiling and outside with only the mullion to act as a heat collector. Seems like quite

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 8:29 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Yes. Steve Leyton Protection Design Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED

RE: Window Sprinklers

2008-10-01 Thread John Drucker
, NJ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 10:28 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The window sprinkler was tested using the exact same criteria as is used

RE: Window Sprinklers

2008-10-01 Thread Russell
Just a note about the mentioning of sprinkler activation. The data sheet states that the advantages are its ability to wet the entire glass and the quick activation time. Well, that quick activation time is a mystery to me because the data states that there is no specific distance below the

RE: Window Sprinklers

2008-10-01 Thread Thom McMahon
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 9:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers So the test assumes the glass remains intact until sprinkler activation? Ron Fletcher

RE: Window Sprinklers

2008-10-01 Thread R Richardson
I believe the issue is similar to in-rack sprinklers in that the activation is more or less direct flame impingement. If there is enough heat to jeopardize the side of a building the head will likely activate. Rich Richardson Seattle Fire Department Russell [EMAIL PROTECTED] 10/01/2008 09:49

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
Protection Design Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a note about the mentioning of sprinkler

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
sprinkler has activated. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a note

RE: Window Sprinklers

2008-10-01 Thread Justin Reid
] -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a note about the mentioning of sprinkler activation. The data sheet states

RE: Window Sprinklers

2008-10-01 Thread Craig.Prahl
, October 01, 2008 1:08 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers That was my point exactly. Not how to install the head per the listing. A manual system would be more dependable than a closed head system with no heat collection. Here's a what if. What if there's a fire

RE: Window Sprinklers

2008-10-01 Thread John Drucker
Sent: Wednesday, October 01, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 2006 IBC 704.12 provides for exterior window opening utilizing a water curtain. Exception - Opening protectives are not required where the building is protected throughout by an automatic

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers If that happens what's the problem? If FD is on the scene and attacking the fire then most likely occupants are out, hose streams are in play and sprinklers at the glass are a non-issue. What about the other sprinklers

RE: Window Sprinklers

2008-10-01 Thread Russell
Rated glass walls have been used for ages but the Tyco window sprinkler is fairly new so I've been wondering what has been done in the past to address this issue architecturally wise. I called an architect and questioned him on it. He said that a long time ago one could use wire glass. Now he uses

RE: Window Sprinklers

2008-10-01 Thread Chris Cahill
be provided. John Drucker Fire Protection Subcode Official (AHJ) Red Bank, NJ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Wednesday, October 01, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 2006

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Rated glass walls have been used for ages but the Tyco window sprinkler is fairly new so I've been wondering what has been done in the past to address this issue architecturally wise. I called an architect and questioned him

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
Of Steve Leyton Sent: Wednesday, October 01, 2008 10:08 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The obvious answer would be heat that directly threatens the glass; a sprinkler could react directly to heat on the same side or to heat radiated from the other side. If it's

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
The Tyco head is specifically listed to provide protection equivalent to a two hour rated assembly. So if the corridor is a rated exit corridor then you need to use the Tyco head to maintain the integrity of the separation. There is no equivalent rating for sprinklering a window with just an

RE: Window Sprinklers

2008-09-30 Thread Fletcher, Ron
If the AHJ will approve closely spaced sprinklers you should be okay. The Tyco window sprinkler has some severe limitations like no horizontal mullions which translates to no doors. Just because a sprinkler is UL Listed for an application it doesn't mean it's the only thing that can be used. We

RE: Window Sprinklers

2008-09-30 Thread Chris Cahill
Cause there is nothing in the code that I am aware of that gives a rating with ordinary sprinklers at any spacing. The 6' comes in about openings in floors and as an alternate in the atriums. These are two specific situations addressed but not a general 1 hr rating. The floor opening has

RE: Window Sprinklers

2008-09-30 Thread Scott A. Futrell
PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 30, 2008 7:59 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers If the AHJ will approve closely spaced sprinklers you should be okay. The Tyco window sprinkler has some severe limitations like

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
: Window Sprinklers If the AHJ will approve closely spaced sprinklers you should be okay. The Tyco window sprinkler has some severe limitations like no horizontal mullions which translates to no doors. Just because a sprinkler is UL Listed for an application it doesn't mean it's the only thing

RE: Window Sprinklers

2008-09-30 Thread Fletcher, Ron
Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Tuesday, September 30, 2008 6:03 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Cause there is nothing in the code that I am

RE: Window Sprinklers

2008-09-30 Thread Fletcher, Ron
] [mailto:[EMAIL PROTECTED] On Behalf Of Scott A. Futrell Sent: Tuesday, September 30, 2008 6:16 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The Tyco limitations are because that is what is required to keep the glass intact, make the sprinkler work properly, and ensure

RE: Window Sprinklers

2008-09-30 Thread R Richardson
That is how we do it in Seattle, just as Chris says. Rich Richardson Seattle Fire Department Russell [EMAIL PROTECTED] 09/30/2008 06:58 Let me see if I understand Chris, from an architectural standpoint, the glass wall is not a rated wall unless the Tyco sprinkler is used? Cause there is

RE: Window Sprinklers

2008-09-30 Thread Russell
Let me see if I understand Chris, from an architectural standpoint, the glass wall is not a rated wall unless the Tyco sprinkler is used? Cause there is nothing in the code that I am aware of that gives a rating with ordinary sprinklers at any spacing. If you have a corridor that requires a

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
, September 30, 2008 9:59 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Let me see if I understand Chris, from an architectural standpoint, the glass wall is not a rated wall unless the Tyco sprinkler is used? Cause there is nothing in the code that I am aware

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers It's permitted this way so what's a fellow to do? Tell the Architect/Engineer, Building Department, Fire Department and owner that they have to eliminate the doors and horizontal mullions from 80 ft. of glass wall? And by the way, the next

RE: Window Sprinklers

2008-09-30 Thread Russell
listed Craig L. Prahl, CET listed appears to be the key word here. I just received a phone call from a representative of Tyco and in essence this sprinkler is better technology and is an option and not mandatory. Thank everyone for your response to my post. As usual they are a great help.

RE: Window Sprinklers

2008-09-30 Thread Fletcher, Ron
@firesprinkler.org Subject: RE: Window Sprinklers Let me see if I understand Chris, from an architectural standpoint, the glass wall is not a rated wall unless the Tyco sprinkler is used? Cause there is nothing in the code that I am aware of that gives a rating with ordinary sprinklers at any spacing

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers listed Craig L. Prahl, CET listed appears to be the key word here. I just received a phone call from a representative of Tyco and in essence this sprinkler is better technology and is an option and not mandatory. Thank everyone

RE: Window Sprinklers

2008-09-30 Thread Russell
Ron, there are vertical mullions spaced at 4' and one door. There are no details or interior elevations for this wall so this is all the info I have without contacting the architect which is my next step. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601

Re: Window Sprinklers

2008-09-30 Thread Roland Huggins
Well actually there is ONE reference in the codes for using spray sprinklers and glass. It is in NFPA 101 - Life Safety Code under Atriums and applies to a 1 hr separation. The trick there is ensuring the set-up is wetting the entire surface. From this humble beginning, it has been a

RE: Window Sprinklers

2008-09-30 Thread Chris Cahill
: Tuesday, September 30, 2008 9:27 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers That's correct, not mandatory but an excellent and tested item. So as long as you can prove that your sprinkler protection of the glazing provides a fire resistant rating equal to that of the wall

RE: Window Sprinklers

2008-09-30 Thread Steve Leyton
: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 30, 2008 6:55 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers It's permitted this way so what's a fellow to do? Tell the Architect/Engineer, Building Department, Fire Department

RE: Window Sprinklers

2008-09-30 Thread Steve Leyton
To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Well if it's not mandatory could someone provide the code reference to another solution for a RATED GLASS WALL? We know how to do unrated and know how to do non-glass. Chris -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: Window Sprinklers

2008-09-30 Thread Steve Leyton
, September 30, 2008 7:54 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers A HA!!! That's the point, isn't it? That the architect failed to completely design the building and account for the protection of windows and likely, the limitations of the window sprinklers in terms