Subject: RE: check valves on dry standpipes
That is very interesting. I wonder what is the reason one is required?
Steve?
John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number
Another thought that you triggered with the term free standing: FDC's
can be composed of single clapper and multi-clapper Siamese bodies, or
built out of manifolds with separate snoots for each inlet, including
snoots with spring checks built into them. So the configuration of the
inlet
Anyone know of a LISTED welded outlet fitting rated 400psi? Have only
found 300psi to date ...
Hey Brad, you have an algorithm to predict burst strength on a 300psi
fitting ... er, no. Wait. Don't. Never mind.
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Tuesday, May 07, 2013 2:27 PM
Concur. My guess is that you could go 4:1 on a groove-o-let up to the same
rating as a Vic 75. Ironically, if we can't find a welded solution to
satisfy this very particular AHJ, then we will use grooved saddles which
are listed for the same working pressure as the couplings attached to
them.
We see this condition quite a lot and we protect above and below.
Steve Leyton
Brian Harris bhar...@bvssystemsinc.com wrote:
All-
Working on a project that has a suspended slatted wood ceiling in the
lobby. The ceiling is made up of 4 wide wood strips with ½ gap in
between each slat, I
, but the overall quality of reclaimed water is controlled by the
water purveyor. You may want to contact them about the level of
suspended solids or other adulterants.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun
% is the most popular, I think ...
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Bobby Gillett
Sent: Monday, May 13, 2013 10:19 AM
To: sprinklerfo...@firesprinkler.org
Subject: Sizing
That's only part of it: you size the tank for the greater of
(sprinklers + HSA) or the fire flow demand, whichever is greater when
calculated as flow x duration.
Steve L.
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
Still not semantically correct. You don't have to proved fire flow
and sprinkler demand concurrently. Sprinkler demand is calculated as
(sprinkler design area + hose stream allowance) x duration. Fire flow
is just fire flow. You determine the most demanding and the water
supply volume has to
Greenman
Sent: Monday, May 13, 2013 10:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sizing tanks with hydrants?
Won't fire flow always exceed sprinkies and hose allowance?
On Mon, May 13, 2013 at 10:35 AM, Steve Leyton
st...@protectiondesign.comwrote:
That's only part of it: you
Game and fire sprinkler density
upgrades ...
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Johnson, Duane (NIH/OD/ORS) [C]
Sent: Monday, May 13, 2013 11:12 AM
To: sprinklerforum
In traditional architectural terms a lintel is the piece between two
vertical supports over a portal, so it could (and often is) used to
describe the header span not only over doors but also windows.
SML
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
So this lens creates a flat and continuous projection along the plane of
the underside of the roof? Agree that you don't need a sprinkler in
the skylight ... unless you consider the space above the lens to be a
combustible concealed space.
Steve Leyton
-Original Message-
From
one valve, break it up into 3 or 4
smaller valves, to diffuse the thrust of that 2,000 gpm inflow. And
pipe fill lines horizontally across the tank to the other side, so that
water drops in as far away from the pump suction fitting as possible.
Steve Leyton
-Original Message-
From
Chris forgot to ask where babies come from. The answer - as I understand it -
to the 52,000 sq. ft. question is ... mildly amusing.
SL
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of George Church
Sent: Tue 5/21/2013 1:58 PM
To:
/interior audible alarm device, please send me that info off
forum at your very earliest convenience. If such an item doesn't yet
exist, perhaps the good people at Potter or System Sensor or another
manufacturer will see a business opportunity ...
Steve Leyton
-Original Message-
From
Sorry for the late chime in - I'm (theoretically) on vacation and don't have
NFPA 20 with me.
As already stated, the 20 yields to other standards that may incorporate a fire
pump into an approved water supply - 13, 14, 24, etc. Where 20 ends isn't
defined, but the discharge control valve
Of course not. Don't let logic interfere with perfectly good regulatory
thinking.
Steve
Mark A. Sornsin, P.E. masorn...@kfi-eng.com wrote:
Is there any concern about water runoff from hose streams in the event the
fire sprinkler system was shut off during a fire?
Mark A. Sornsin, P.E. |
I've been hanging blinds, and just now have the time to note this most
extraordinary turn of the thread. I got nothing - this may be the greatest
correspondence in the history of the Forum.
Remember back in 1997 or thereabout, when an errant email home from some kid in
the Midwest (no, not
. The MEOR should do a quick look-see calc' to assure that
there isn't excessive friction loss from the sleeve(s) in the stream.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf
Be sure they're not on the downstream side of domestic regulators.
SL
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of Todd - Work
Sent: Wed 6/19/2013 6:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: water test without hydrants
I am
That's a funny statement, We can't have glass bulbs. Why is that,
because an architect said, No glass bulbs?
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rfletc
of spending time with him - and Cathy - away
from business, away from the stress. He was a really good guy; what
you saw was what you got. One of the two or three most sincere and real
people I will ever know, and I'm going to miss him very much.
Steve Leyton
-Original Message-
From
Those are mechanical restrictors that only operate on residual pressure. If
system pressure doesn't exceed 175 psi, the prescriptive code says you don't
need them, but it's a good idea to check with the responding fire dept. just to
be sure they're okay with regular valves and the existing
Also if there's storage. We're working with two large 26' high walk-ins
currently.
Steve
Richard Carr rc...@coxfire.com wrote:
Yes, they have a defrost mode that will pop a head of 155 deg.
Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
What Richard said.
Steve
Richard Carr rc...@coxfire.com wrote:
As long as you call the gate on the BFP your system control valve and
underground is rated for 200, you should be fine, see it all the time.
Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville,
I meant to say, ... EVEN if said equipment is gas fired in the last
sentence.
Steve
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steve Leyton
Sent: Wednesday, July 17, 2013 11:32 AM
Thank you for that good news and a hoorah to the NJ legislature.
Steve
John Drucker - Home john.druc...@verizon.net wrote:
Members
Today the State of New Jersey, Department of Community Affairs, Division
of
Codes and Standards issued a guidance document to code officials with
regards to home
Yes, but if it's not rated I would say you need to do a design for EH II that
encompasses the booth, the mixing room, and adjacent spaces (assuming no 2-hour
separations from adjacent uses) up to the required design area in 11.2.3.1.1.
Steve Leyton
Protection Design Consulting
San Diego, CA
it will make a big difference in the water
supply and storage.
J.P. Merlino
-Mensaje original-
De: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] En nombre de Steve
Leyton
Enviado el: viernes, 26 de julio de 2013 02:10 p.m.
Para
Gustin-Bacon perhaps?
Steve
Mike Hairfield fsl...@msn.com wrote:
I remember the Riken Top Brand Line but they were gray, but the same take-outs
as Vic.
Mike
Subject: green grooved fittings
From: t...@fpdc.com
Date: Fri, 26 Jul 2013 11:07:19 -0400
To:
, IBC, IMC, and adopted
electrical code.
Was the booth installed under benefit of permit?
bv
- Original Message -
From: Steve Leyton st...@protectiondesign.com
To: sprinklerforum@lists.firesprinkler.org
Sent: Friday, July 26, 2013 12:14:37 PM
Subject: RE: Paint booth
Not sure there's
The required flow is the highest system demand. This has been in 25 for
(somebody help me out here) at least two cycles, I believe? You can
use the main drain if you can develop enough flow, you can modify the
main drain connection possibly to create multiple connections, you can
modify and
a permit
I simple chart would be awesome - IN THE BOOK - so we have something
to point to.
Greg
On Mon, Jul 29, 2013 at 4:36 PM, Steve Leyton
st...@protectiondesign.com
wrote:
The required flow is the highest system demand. This has been in
25
for
(somebody
a 2
main drain is fine for everything, some say prove the size before you
pull a permit
I simple chart would be awesome - IN THE BOOK - so we have something
to point to.
Greg
On Mon, Jul 29, 2013 at 4:36 PM, Steve Leyton
st...@protectiondesign.com
wrote:
The required flow
Zachary. If Ben's a true Ponderosan, he's organically opposed to paying taxes
at all, let alone higher taxes. The cost of fire to our communities is too
high for the revenue bases that fire departments have to work with. Response
times are getting longer. Some cities with extraordinary
Research Foundation's latest study, go here:
http://us1.campaign-archive1.com/?u=d425222efb214106f8a57d073id=49a2700
1cee=5f66fc5dce
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South, Suite 400
San Diego, CA 92108
My BAD It's a $115 fee ... the freebie was Monday and I
apologize for butchering that.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steve Leyton
Sent: Wednesday
Zachary. Unless it was furnished by the manufacturer less valves. But my
understanding is they can't do that because there's no way to test it
according to the USC method for certification.
Steve
John Denhardt jdenha...@stricklandfire.com wrote:
With no control vale on the discharge of the
-certifications as required by most water
districts.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Tony Silva
Sent: Thursday, August 01, 2013 10:03 AM
To: sprinklerforum
Help a warm weather brother out please, with recommendations for heat
trace systems. Price, reliability, branch line listings?
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South, Suite 400
San Diego, CA 92108
- this was a big system in a 100'-0+ tower
w/standpipes etc.. It ended up needing two panels for supervisory due to
the length of the cables, etc.
Bobby
On Thu, Aug 1, 2013 at 1:53 PM, Steve Leyton
st...@protectiondesign.comwrote:
Help a warm weather brother out please, with recommendations for heat
trace
a drum drip at the other end? 1/4 per 10'
of main = 2 1/2 in 100'
Thanks,
J. Lewis
From: Steve Leyton st...@protectiondesign.com
To: sprinklerforum@lists.firesprinkler.org
Sent: Thursday, August 1, 2013 12:15 PM
Subject: RE: Heat trace question
allowed in 13/2013-7.1.3?
On Thu, Aug 1, 2013 at 12:15 PM, Steve Leyton
st...@protectiondesign.comwrote:
These are two isolated areas at a hospital - one over some outdoor
seating at the dining common and the other a canopy that covers trash
enclosures and a couple of service enclosures. Both
: (407) 656-8026
www.waynefire.com
Celebrating over 34 years of life safety
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, August 01, 2013 1:15 PM
Dude has egress issues.
Let's see, a 97' tall structure made entire of wood with uneven flooring and
absolutely no consideration made to any applicable code, apparently. And the
media coverage is of the FM-as-Grinch. I mean, what could go wrong?
SL
-Original Message-
From:
The article said that the closing of the building disappointed the hundreds of
visitors he gets. I'd say that people wandering around in a non-compliant
10,000 sq. ft. tinderbox, presumably without compliant exits, signage, occupant
notification, sprinklers, etc., etc., etc. would trump
exceeds 5,000 sq. ft., contains more than a fire area
with a Group A-2 occupancy, and is separated into two or more buildings
by fire walls of less than four hour fire resistance rating without
openings.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
cursing in Spanish? Watch a finishing
crew that has to meticulously mud sheetrock up to the firestop
assemblies at each of the dozens of drops that penetrate that one-hour
lid at the top of the plenum space.
Steve Leyton
-Original Message-
From: sprinklerforum-boun
as well.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Roland Huggins
Sent: Monday, August 05, 2013 1:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Special
of the dwelling units).
The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.
Steve Leyton
Protection Design Consulting
San Diego, CA
-Original Message-
From: sprinklerforum-boun
to buildings that are taller than the responding
FD's capacity to pump.
The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 14 Technical Committee on Standpipe and
Hose Systems.
Steve Leyton
Protection Design Consulting
San Diego, CA
connections, as justified it as being capable of
supply from two different legs of the muni system.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Johnson, Duane (NIH/OD/ORS) [C]
Sent
codified an amendment that requires at least 30 minutes
of standpipe water. In Los Angeles, they require standpipe demand x
highest sprinkler hazard class duration, so if you have OH parking or
retail you have to go 750 or 1000 x 60 minutes and you get some pretty
big reservoirs.
Steve Leyton
don't oppose that approach.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Martinez, Dewayne
Sent: Tuesday, August 13, 2013 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
I wish I had a pat answer for you, but it's going to vary from AHJ to
AHJ. This has been a topic of conversation on FPO chat forums here.
SML
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Geza - will you please send that directly to me off-forum? AFSA list-server
doesn't do attachments.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Geza
Szakats
Sent
, please contact Cecil at your
earliest opportunity.
URL: www.sprinkleracademy.com
Email:ce...@sprinkleracademy.com
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South, Suite 400
San Diego, CA 92108
the various tube and
spring assemblies, I'd wager they've got the net K or pressure loss available.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of Matt Grise
Sent: Thu 8/15/2013 6:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE
We've used it in residential wood-framed buildings near Beaumont.
Steve L.
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Brad Casterline
Sent: Wednesday, August 21, 2013 12:37 PM
To:
Is a C-channel or Z-channel that you're asking about? The term purlin
can refer to the shaped members commonly used in engineered structures,
but by definition a purlin is any member that is born by the primary
members (beams, girders, trusses) and which directly bears either the
roof or smaller
-purlins.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steve Leyton
Sent: Monday, August 26, 2013 11:36 AM
To: sprinklerforum
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steve Leyton
Sent: Monday, August 26, 2013 11:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Hanging from Purlins
As others have said
?
Thanks,
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South, Suite 400
San Diego, CA 92108
-
Ph: 858.751.2930 - ext. 102
Fax:858.751.2933
Cell: 619.972.5696
: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Monday, August 26, 2013 12:59 PM
To: sprinklerfo...@firesprinkler.org
Subject: Remote fire pump start
I was asked about this product and fail to see any real value
I've been on an airplane, so couldn't respond but ... what he said.
SL
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org on behalf of Roland Huggins
Sent: Fri 8/30/2013 10:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Protecting Pipe in
What kinds/quantities of chemicals? Flammable gasses? This is so
subjective ... it could be an EH II just as surely as an OH II.
Steve Leyton
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf
fell - the pix
tell a compelling story.
Steve Leyton
PROTECTION DESIGN CONSULTING
2851 Camino del Rio South, Suite 400
San Diego, CA 92108
-
Ph: 858.751.2930 - ext. 102
Fax:858.751.2933
Cell: 619.972.5696
http
or more. As bad
as things were 4 years ago, this is looking a lot worse.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Monday, October 22, 2007 1:52 PM
To: sprinklerforum@firesprinkler.org
Right. Except for the fact that there are about 15,000 homes directly
in harm's way, some of them perhaps occupied by environmentalists.
These aren't really wildland fires; they have moved quickly from grassy
foothills into the suburbs. The forest management debate will have to
wait for
At this exact moment, all of them.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Tuesday, October 23, 2007 7:19 AM
To: sprinklerforum@firesprinkler.org
Subject: horror averted
Ran
Here's a good one:
In Idaho:
Sprinkler system helps contain fire at NNU dorm
10/23/2007
KTVB
BOISE -- Nampa fire officials credit a sprinkler system from preventing
a major fire disaster in a dormitory at Northwest Nazarene University
this morning.
Firefighters got a call from an
have ordinance or policy regarding
arrangement of water supplies in shorter buildings than high-rise. But
so long as you don't exceed 52K s.f. of area per floor, you only need
one system.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
of the
split.
Usual disclaimer, my opinion only ...
Steve Leyton
Away from the office - sent from my BlackBerry
-Original Message-
From: Karen Purvis [EMAIL PROTECTED]
Date: Mon, 5 Nov 2007 12:25:51
To:sprinklerforum@firesprinkler.org
Subject: Standpipe Zones
Can anyone give me
If it's a high-rise, you'll need two FDC's, but it will still be a single zone
as George says. As for deferring, all I can say is give him room on the
hairpins.
My opinion only ...
Steve Leyton
Away from the office - sent from my BlackBerry
-Original Message-
From: George Church
were concerned about draggiong the fire official into the
design process. I'd be happy to write it up again with you.
Steve Leyton
Away from the office - sent from my BlackBerry
-Original Message-
From: Greg McGahan [EMAIL PROTECTED]
Date: Tue, 6 Nov 2007 06:57:23
To:sprinklerforum
that could be divided up
horizontally to cover different portions of a building, but in terms of
the 14 and the definitions therein, it's not a zone.
Steve Leyton
Protection Design Consulting
The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems
be provided at the proscenium to protect the separation between a
legitimate stage and the A-group.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Randy Knutson
Sent: Thursday, November 08, 2007 5:28 PM
Randy:
We're all secretly e-mailing each other but leaving you off the list.
Need-to-know basis ...
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Randy
Knutson
Sent: Friday, November 09, 2007 3:53 PM
, exterior walls, etc. such that you minimize
underground piping under the building (10.6.4)
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, November 13, 2007 6:20 AM
saw there the
morning after the fire, I'd be hard-pressed to justify changing the existing
provisions.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, November 13, 2007 1:22 PM
the EOR is smoking so that I can at least try to get on the
same page as the design team?
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 14, 2007 12:41 PM
To: sprinklerforum
the exception of sprinklers in attics, closets, bathrooms,
etc.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Friday, November 16, 2007 11:48 AM
To: sprinklerforum@firesprinkler.org
Subject: 13 vs
You mean by a noose?
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Sean
Conlin
Sent: Friday, November 16, 2007 8:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Its Friday and I am a sprinkler man
and the sumbitch blew completely out of the ground
according to witnesses. But the extent of the damage to the pipe was
awesome.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Wednesday
(i.e. the NAHB, for ex.) will give him a venue and an
audience. Our good friend, the late Bob Caputo and my SoCal buddy Ken Wagoner
have both had their day with this fellow and they came out of the experience
with anger issues and a foul odor about them.
Steve Leyton
Protection Design
.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Miller
Sent: Friday, November 30, 2007 6:52 AM
To: sprinklerforum@firesprinkler.org
Subject: Commercial Condos - Control Valves for Tenant Spaces
in Las Vegas where it catastrophically freezes once every
10 years or so. We really appreciate you looking after us as always.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Tuesday, December 04
system, should suitable for
primary streams and attack lines, which pretty much takes small hose
stations and Class II connections out of the equation. This isn't the
classic mop up application ...
Steve Leyton
Protection Design Consulting
The foregoing is my opinion only and is not intended
for
fast attack (in a sprinklered warehouse?) then a class I would the
one. Of course, as Steve says, the standpipe is for the FD and it's
their requirement that needs to be met.
On Dec 5, 2007 1:47 PM, Steve Leyton [EMAIL PROTECTED] wrote:
In a word, no. Methinks that you would go to the applicable
Sounds like exposed unexpanded, with a building height of 40'. I think
the pitch is okay for ESFR, so try K25 at 50 PSI. And bring your pump.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kevin
Pugh
Sent
You're right - I just stopped looking at Table A-2 after the first
column ...
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Thursday, December 06, 2007 9:55 AM
To: sprinklerforum
I think the point is to tape and dope the inspector ...
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gary
Stites
Sent: Friday, December 07, 2007 8:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Tape
Hmmm, you want to write him back and ask him about the particulars or
does this fall into the category of polishing a turd?
(Sorry Munce - for more on polishing, see AFSA's seminar program ...)
:o)
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED
I've seen it too! Rats and mice can sense that there's water in the tubing;
where I saw it the pipe was CPVC.
Steve Leyton
Away from the office - sent from my BlackBerry
-Original Message-
From: Mike Brown (TECH- GVL) [EMAIL PROTECTED]
Date: Fri, 14 Dec 2007 12:23:22
Funny, but not. If you saw the fatality statistics from the latest
storms across the country, the breakdown includes categories such as
Automobile-Related; Heart Attack and Indirect Medical; Trauma and ...
Carbon Monoxide Poisoning.
Steve Leyton
Protection Design Consulting
-Original
We've done this on many projects, but to my knowledge it was always
blown in.
Steve Leyton
Protection Design Consulting
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, December 19, 2007 9:13 AM
To: sprinklerforum