[Sprinklerforum] Re: Storage Unit Inspections

2024-08-15 Thread Ron Greenman
Jennifer, Note that it is the owner's responsibility to provide access, not the inspector's. The inspector is responsible for what he/she has access to. In the case of the sprinklers themselves, the inspector is responsible for visually inspecting those that can be readily seen from the floor. A g

[Sprinklerforum] Re: Storage Unit Inspections

2024-08-14 Thread Ron Greenman
Here is a quote from an information sheet I made for owners quoting from the 2014 edition of 25. I've not been playing since around 2019 so I have not updated it since that 2014 edition. I don't know what edition you're using or if the wording has changed since 2014, I would think that if you inclu

[Sprinklerforum] Re: Gym Hazard Classification

2024-07-21 Thread Ron Greenman
This goes back a ways and the wording may have changed over the editions but here it clearly differentiates between owner and contractor and who does what and when. “4.3* Owners Certificate. The owner(s) of a building or structure where the fire sprinkler system is going to be installed or their a

[Sprinklerforum] Re: Suction Control Valve

2024-04-13 Thread Ron Greenman
I would guess that anyone here who knew George misses him. And in the spirit of George, anyone reading this who finds the forum useful and is not a member of AFSA ought to join before the day is done. And also join your local chapter. On Sat, Apr 13, 2024 at 10:10 AM wrote: > We need a ‘smiley

[Sprinklerforum] Re: Protecting underground storage of explosives.

2024-04-06 Thread Ron Greenman
https://codes.iccsafe.org/content/IFC2018/CHAPTER-56-EXPLOSIVES-AND-FIREWORKS?site_type=public On Sat, Apr 6, 2024 at 1:20 PM Prahl, Craig wrote: > Munitions and explosives are typically protected via separation. On > military projects, storage areas such as these are either semi-subterranean >

[Sprinklerforum] Re: Sidewalls on curved walls

2024-03-08 Thread Ron Greenman
I'm thinking this may be one of those occasions where that PE after your name may need to be summoned, Todd. On Fri, Mar 8, 2024 at 11:22 AM Fpdcdesign wrote: > Light Hazard. Waiting room > > > > On Mar 8, 2024 at 2:18 PM, > wrote: > > What’s the occupancy of the space? > Rick Matsuda > > On Mar

[Sprinklerforum] Re: Dry Sprinkler Heads

2024-02-06 Thread Ron Greenman
According to this article... 1937. https://www.sprinklerage.com/dry-barrel-sprinklers/#:~:text=The%20first%20UL%2Dlisted%20dry,three%2Dquarters%20of%20a%20century . On Tue, Feb 6, 2024 at 3:12 PM James Crawford wrote: > I was asked today when the first dry heads came into use and did not have >

[Sprinklerforum] Re: AFSA ITM Connection - Sprinkler head security cameras

2023-11-16 Thread Ron Greenman
Suppose you're in a store and you find something like this. Doesn't look like the rest of the sprinklers in the place, are only in dressing rooms, and in each space, there is one of these and one of the regular sprinklers found throughout the building. You tell the manager as he's the likely highes

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Ron Greenman
John D. Remember when we used to zone each level of a dry pipe system in open parking garages with a check valve to speed up trip time, or am I really showing my age? Could each level of Ken's project be connected to a single pipe, with or without a check valve that ran to the top and a single air

[Sprinklerforum] Re: Pump Suction Components

2023-09-12 Thread Ron Greenman
I think, a dangerous thing, and based totally on speculation, without any supporting information, the grv x flg could be used due to vibration. I can visualize something as heavy and lopsided as an OS&Y rotating. Again, just pure speculation. On Tue, Sep 12, 2023 at 6:31 AM Brian Harris wrote: >

[Sprinklerforum] Re: [EXTERNAL] Re: Sprinklers in column enclosures

2023-08-08 Thread Ron Greenman
I hate to solve technical problems that aren't really problems by adding cost to a jib but if the BI is not going to budge change the wood framing design around the columns to steel and you have a non-combustible concealed space. Or if already framed go with Chris' suggestion. I once had an AHJ war

[Sprinklerforum] Re: Optional sprinkler protection in garage without sprinklers elsewhere

2023-07-06 Thread Ron Greenman
I think this situation fails to fall under the guidance of any code or standard. I think the owner needs to define what he is trying to accomplish since he seems to be the driver for this voluntary solution to a vaguely defined problem. The building code already demands a more robust fire separatio

[Sprinklerforum] Re: Fire Station Apparatus Bay

2023-02-16 Thread Ron Greenman
Given those two choices, I'd say a showroom is pretty devoid of fully fueled cars and that they are spaced far enough apart for customers to easily navigate around. An FD apparatus bay is filled with fully fueled vehicles that are started in the bay. The bay also contains lots of ancillary gear. I'

[Sprinklerforum] Re: 13R: Hotel Corridors Open to Lobby

2022-12-15 Thread Ron Greenman
If I'm picturing this one way I'd say if there was no separation other than visual like a valance, a floor elevation difference, or a change of carpet pattern then there is no corridor. If in another visualization where there is a corridor to either side of a wide opening from the lobby then the QR

[Sprinklerforum] Re: BFP on underground supply

2022-11-18 Thread Ron Greenman
Being semi/mostly out of the game I don't keep as up-to-date as I maybe should be and so I don't have too many standards left having donated many to those still in need. So my question is where is the requirement mentioned? 13, 24, 25, all? That should be a guide as to who is ultimately responsible

[Sprinklerforum] Re: plans and specifications vs design build

2022-11-18 Thread Ron Greenman
Didn't you say this was a firehouse? Maybe get the fire marshal involved. If an engineer stamped the plans and gave those out as what to bid on then if you win the contract you build to what the engineer said. Who are you, lowly contractor/engineering tech to argue with the mighty PE? But if he's w

[Sprinklerforum] Re: Center vs Quad

2022-10-24 Thread Ron Greenman
Travis, I've had that same conversation dozens of times. On Mon, Oct 24, 2022 at 1:44 PM Brian Harris wrote: > Travis- > > I like it…. > > > > *Brian Harris, CET* > > BVS Systems Inc. > > bvssytemsinc.com > > > > ** Please “Reply All” To Email Correspondence ** > > >

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Ron Greenman
Is this new addition a "proper" separate building or just another fire area. If the former your solution of a booster pump for just the EFSR "building" tapped from the main UG line sounds like a good solution. If just a fire area Ken's comment about FDC feeds after the pump is spot on. I'd also thi

[Sprinklerforum] Re: Adding sprinklers to system with mixed SR/QR listing

2022-09-27 Thread Ron Greenman
Fast response elements do not universally equate to quick response sprinklers. https://www.vikinggroupinc.com/sites/default/files/documents/Automatic%20Sprinkler%20Thermal%20Sensitivity.pdf On Tue, Sep 27, 2022 at 10:58 AM Matthew J Willis wrote: > Todd, > > > > What are you protecting? > > > >

[Sprinklerforum] Re: Adding sprinklers to system with mixed SR/QR listing

2022-09-26 Thread Ron Greenman
I'm old now so you get a story first, probably with a divergence (and there it is already and again), but Grinnell made a sprinkler that had different K-factors depending on the height it was placed at (9.0, 9.2, 9.4, etc.). An AHJ once called me out for using 9.0 in a calculation whose height fell

Re: Vertical Wet Pipes in Dry Attic

2022-03-02 Thread Ron Greenman via Sprinklerforum
Not directly related but Scott’s answer gave me pause. Just as new designers should spend a couple of weeks or more with fitters sneaking questions and getting a handle on what works for them, companies that also do inspections should have their designers go out with the inspectors. And often. Actu

Re: Joining black carbon steel with stainless steel piping

2022-02-28 Thread Ron Greenman via Sprinklerforum
Food for thought... https://www.eng-tips.com/viewthread.cfm?qid=351636 On Mon, Feb 28, 2022 at 8:30 AM Fpdcdesign via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > > > > The last dielectric joint I saw was a 9” piece of CPVC > > > > > > > > > > > > > > On Feb 28, 2022 at 11:

Re: Sprinkler in elevator pit.

2022-02-25 Thread Ron Greenman via Sprinklerforum
May be helpful. Maybe not. https://www.nfpa.org/News-and-Research/Publications-and-media/Blogs-Landing-Page/NFPA-Today/Blog-Posts/2019/11/20/101wednesdays-vertical-opening-protection-in-nfpa-101 On Fri, Feb 25, 2022 at 7:01 AM Ken Wagoner via Sprinklerforum < sprinklerforum@lists.firesprinkler.or

Re: filling a pre-action system with water

2022-02-17 Thread Ron Greenman via Sprinklerforum
Water hammer occurs when flow is abruptly stopped. On Thu, Feb 17, 2022 at 12:20 PM Art Tiroly via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > The high pressure water in=rush compresses the air in the system. > The velocity slows as the air pressure is compressed. I don't be

Re: [EXTERNAL] RE: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread Ron Greenman via Sprinklerforum
What John said. On Mon, Feb 7, 2022 at 6:11 PM Tom Duross via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Doing some commissioning work on a new one for New Balance here in > Boston. Building shaped like a peanut, curved walls and roof. Almost > every space is OH2, large s

Re: question about Storage height

2022-01-26 Thread Ron Greenman via Sprinklerforum
Did I miss something? I thought you said 5 groups of 5x5x5 cubes stacked 2 high. That's only 125 sqft. Wouldn't it be cheaper to make a separate space, either with two hour walls or to just extend the coverage beyond the area with the higher demand as per NFPA. The solution seems so obvious and sim

Re: [EXTERNAL] Re: Food trucks inside a building

2022-01-14 Thread Ron Greenman via Sprinklerforum
I can't get over the cooking aspect. If this were a burger stand there would likely be a deep-fat fryer, a griddle, perhaps a grill, and a range top. I imagine a taco stand would be similar and so also a taco truck. In any event greasy vapors for all and a cooking line fire suppression system. A fo

Re: COMBUSTIBLE CONCEALED SPACE

2022-01-13 Thread Ron Greenman via Sprinklerforum
For every problem there is a solution that is obvious, simple, and wrong. On Wed, Jan 12, 2022 at 7:13 AM Ken Wagoner via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Indeed Travis and I have journeyed down this road before, one time in > particular. > > An AHJ, who happened

Re: Food trucks inside a building

2022-01-13 Thread Ron Greenman via Sprinklerforum
Then there are the greasy vapors the taco trucks, times six fast food kitchens are spewing out into an enclosed space. I doubt if the trucks are equipped with any kind of grease scrubbers so the clientele are essentially eating under a giant coking line hood (the roof) that may or may not even be v

Re: Liquor above 20% Alcohol Containers less than 1.3 gallons

2021-11-30 Thread Ron Greenman via Sprinklerforum
Sometimes the packaging is the “commodity.“ Something you’ll never see but consider gold ingots individually packed in styrofoam, in cardboard boxes held together with shrink wrap, stacked on plastic pallets, stored in a vault. What’s the…? On Tue, Nov 30, 2021 at 7:33 AM Matthew J Willis via Spri

Re: Clean Agent System

2021-08-23 Thread Ron Greenman via Sprinklerforum
Totally my opinion and worth every penny you're paying for it, if the purpose of closing the dampers is to maintain volumetric integrity of the compartment vis-a-vis the amount of agent I would consider that function to be art of the suppression system and so controlled by the releasing panel. If o

Re: NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking

2021-08-05 Thread Ron Greenman via Sprinklerforum
Considering all the comments: ",,,the vehicle is parked temporarily and a fire starts" (Scott). That could be while I'm still in the taxi settling up with the driver. That would imply stopping is permanent parking. "Merriam-Webster's Collegiate Dictionary, 11th edition, shall be the source for

Re: Material Prices !!

2021-08-05 Thread Ron Greenman via Sprinklerforum
There's also a shortage of port capacity/unlading capability (and I'll assume loading at the other end). The Suez parking debacle put everything using that transit days behind schedule and so tying up those containers and throwing shipping schedules off. Logistics, logistics, logistics. For lack of

Re: Flexible hose head connectors on a pipe schedule system

2021-08-03 Thread Ron Greenman via Sprinklerforum
Passed on to me from a friend. UL IQ. Information for the category VENF - Flexible Sprinkler Hose with Fittings. "These products are intended for use in hydraulically design sprinkler systems." There's more info around it but you'll need to go see for yourself. As Steve said, I'm old, but what h

Re: Flexible hose head connectors on a pipe schedule system

2021-08-02 Thread Ron Greenman via Sprinklerforum
Tyson, While I tend to agree with you and can think of many pipe scheduling rules going back half a century or more that would suggest that flex heads are ad were outside of the scope of a pipe scheduled system I'm curious as to what criteria you're basing your opinion on. At face value, it would

Re: FP Suction Control Valve

2021-07-29 Thread Ron Greenman via Sprinklerforum
I think I’ve preached this before but to my way of think standpipes and hydrants are the drivers of design when present with sprinklers acting as a first line of containment, buying time for manual suppression. That they work so well at suppression so often is an added bonus. On Thu, Jul 29, 2021

Re: Location of hydrant valves in CA.

2021-05-07 Thread Ron Greenman via Sprinklerforum
Not having ever been on any committee making up any rules regarding this I'm going to take some logic shots at the issue as to the whys. If the hydrant is along a right of way then the service valve will be in the street somewhere perpendicular to the direction of the street in a straight line from

Re: Dry System Couplings

2021-05-03 Thread Ron Greenman via Sprinklerforum
t; Futrell via Sprinklerforum > Sent: Friday, April 30, 2021 8:08 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Scott Futrell; Ron Greenman > Subject: RE: Dry System Couplings > > Ron, > How many did you see corroded and leaking that didn't have a tri-seal or >

Re: Dry System Couplings

2021-04-30 Thread Ron Greenman via Sprinklerforum
essage- > From: Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tom Noble > via Sprinklerforum > Sent: Friday, April 30, 2021 8:14 AM > To: Ron Greenman via Sprinklerforum > Cc: Tom Noble > Subject: Re: Dry System Couplings > > NFPA 13 2016 ed

Re: Fire Pump Sprk & Fire Flow Demand

2021-04-21 Thread Ron Greenman via Sprinklerforum
Consider that if the building was not there and you could meet the required CFC fireflow for the site you'd be done, just as you would for any land development project, municipal or private. No pump necessary. Then you reference 13 as the place with the sticky wicket paragraph about everything afte

Re: Shop Drawings vs Design Drawings in Florida

2021-03-29 Thread Ron Greenman via Sprinklerforum
Not just a sprinkler job and sprinklering was not the only piece of contention, but I worked on a job where the architect argued the work was a remodel of the existing one-story mid-60s rambler. What he intended to leave lost in the new work were two e=interior walls and some of the original founda

Re: NFPA 13 2016 25.2.1.4.2

2021-03-19 Thread Ron Greenman via Sprinklerforum
That like button would come in handy with Bruce's comment. There is a lot of misinterpretation because we use the same words for different things. On Fri, Mar 19, 2021 at 9:10 AM Matthew J Willis via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > I am curios, > > Did you includ

Re: Cleveland Automatic Sprinkler

2021-03-18 Thread Ron Greenman via Sprinklerforum
I believe Automatics came out with the first Standard Spray Sprinklers in 1953. The SS had the U (upright) of P (pendant) designation and defined their orientation. The "old-style" sprinklers or conventional sprinklers manufactured before then could be installed in the upright or the pendant positi

Re: Smoke Detectors

2021-03-18 Thread Ron Greenman via Sprinklerforum
I remember something about keeping the detector 12" out and down from the intersection of a wall and ceiling but that had nothing to do with sprinklers and may have been an industry practice, or a "Sven and Ollie we've always done it this way, right-or-wrong" rule. On Thu, Mar 18, 2021 at 7:40 AM

Re: leaving abandoned sprinkler piping in place

2021-03-17 Thread Ron Greenman via Sprinklerforum
"Things like this are precisely why AFSA membership is well worth it." 👍 Here is the conundrum on this type of post. I don't need to weigh in as everyone to the east of me has already answered Travis's questions but I want to thumbs-up Travis' thank you to those that answered as well, and mostly,

Re: Metal Mesh Ceiling tile replacement

2021-03-04 Thread Ron Greenman via Sprinklerforum
I believe the "less than 1/4"" has to do with the depth of the ceiling tile. This rule goes back to at least the seventies and was originally for addressing plastic "egg-crate type tiles." On Thu, Mar 4, 2021 at 8:40 AM David Williams via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wr

Re: Group III Aircraft Hangar

2021-02-19 Thread Ron Greenman via Sprinklerforum
I'm tempted to look at the actual hazard rather than what the commodity is called. Airplane house/garage usually means hanger with the associated hazards, but if you just have aluminium tubes with appendages...? Presumably less activity than a typical warehouse, no combustible liquids like in a par

Activity

2021-02-12 Thread Ron Greenman via Sprinklerforum
Seems like there's been a resurgence in activity in the list recently. Makes me happy and I know it would have made George Church happy. So in the spirit of George, or perhaps channeling George's spirit, if you are an active participant or a lurker that finds value in this exchange and you're a mem

Re: Multiple System Calculation

2021-02-12 Thread Ron Greenman via Sprinklerforum
This sounds like a job for more sheetrock. Oh, and more cowbell is always good. On Fri, Feb 12, 2021 at 10:57 AM Sean Conlin via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > See NFPA-13, 23.4.4.1.1.4 and 23.4.4.1.1.5. > > > > This should help you with the engineer. > > > Rega

Re: Townhome - Common Areas

2021-01-27 Thread Ron Greenman via Sprinklerforum
A clause in the sales contract that that owner of the adjacent unit is responsible, or that all owners that use that common area are equally responsible as in the maintenance assessments associated with HOAs. This is my opinion for a solution way out of the purview of the sprinkler contractor, and

Re: Stand-Alone UPS protection design

2021-01-14 Thread Ron Greenman via Sprinklerforum
I think I'd try to get the building designer to put the UPS into a dedicated enclosure and use an inerting system. On Thu, Jan 14, 2021 at 10:48 AM Prahl, Craig/GVL via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > So, I'll assume this battery assembly will be in some type of

Re: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-10 Thread Ron Greenman via Sprinklerforum
king about this wrongly for a long time. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Thu, Dec 10, 2020 at 10:39 AM Cary Webber via

Re: Event Center Floors

2020-12-01 Thread Ron Greenman via Sprinklerforum
907 <https://up.codes/viewer/wyoming/ibc-2018/chapter/9/fire-protection-and-life-safety-systems#907> . 3. 2.3. An automatic sprinkler system <https://up.codes/viewer/wyoming/ibc-2018/chapter/2/definitions#automatic_sprinkler_system> is provided in storage

Re: Diesel Fuel Tank - Leak Protection

2020-11-20 Thread Ron Greenman via Sprinklerforum
o with the threshold (or I guess in this case the oilhold)? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Fri, Nov 20, 2020 at 3:07 PM BRUCE

Re: Domestic Demands 13R

2020-11-12 Thread Ron Greenman via Sprinklerforum
the junction/split with the domestic and then out to the loop. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Thu, Nov 12, 2020 at 9:03 AM

Re: Clearance around all pump equipment

2020-11-07 Thread Ron Greenman via Sprinklerforum
Pretty much, Ben. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Sat, Nov 7, 2020 at 6:56 AM Ben Young via Sprinklerforum

Re: Clearance around all pump equipment

2020-11-05 Thread Ron Greenman via Sprinklerforum
In one local jurisdiction here there is a requirement for three feet all around major equipment, font, sides, and back. It would good if they would inform the architects that continue to provide smaller and smaller pump and riser rooms. Ron Greenman rongreen...@gmail.com 253.576.9700 The

Re: pharmacy

2020-10-10 Thread Ron Greenman via Sprinklerforum
n the direction they entered), limited exiting, and anything else one can think of regarding the stupidity of the customers, as much as the types and amounts of commodities. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner H

Re: pharmacy

2020-10-09 Thread Ron Greenman via Sprinklerforum
My Big Book of Building Occupancies says drugstores are Group M-Mercantile and Sprinkler Installation Bible says mercantile is ordinary hazard. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film

Re: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-24 Thread Ron Greenman via Sprinklerforum
compressor the switch would need to be a Double Pole/Single Throw. Again. you can't tell from just the lever. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera

Re: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-24 Thread Ron Greenman via Sprinklerforum
t motor or one capable of being locked out if out of sight. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Thu, Sep 24, 2020 at 11:50 AM Mike

Re: Non-Combustible Concealed Space

2020-09-10 Thread Ron Greenman via Sprinklerforum
latter, occupied compartment that is protected. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Thu, Sep 10, 2020 at 12:58 PM rix rixford via

Re: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Ron Greenman via Sprinklerforum
point about being blamed for any problems even if the problem and the work were at opposite ends of the building would thereby be mitigated to perhaps a more bearable risk. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner H

Re: Flexible assembly for Novec 1230 at seismic separation joint

2020-08-17 Thread Ron Greenman via Sprinklerforum
you looked into and rejected, but I've been around the block enough times to know that sometimes the simple solutions tp problems just elude us, so could you use the multi-joint seismic connection from NFPA 13? And when you think, "Of course I have you moron," I'll not ta

Re: 13 R in a single family home

2020-08-13 Thread Ron Greenman via Sprinklerforum
In Washington, there was a guy that required conformance to 24 in stand-alone 13D installations even though it isn't referenced. He was fine with poly, PVC, CPVC, or orange CPVC if it was any type of system that was a combination of plumbing or fire. Ron Greenman rongreen...@gmai

Re: Missing hydraulic data plates

2020-08-06 Thread Ron Greenman via Sprinklerforum
, and the associated cost involved. The same process would apply for a modification to the system. Ultimately, if the information is required it os the owner's responsibility to provide it. How that is accom[lished is the owner's decision. Ron Greenman rongreen...@gmail.com 253.576

Re: Pump or Fire Pump

2020-07-08 Thread Ron Greenman via Sprinklerforum
You might want to put a handwashing sink in the pump room downstream of the pump. It seems like adding one toilet to an otherwise stand-alone sprinkler system, to make it a flow-through system to alleviate the need for a backflow, at least in Washington, turns it into a plumbing system. Ron

Re: [EXTERNAL] RE: Floor area less than required

2020-06-17 Thread Ron Greenman via Sprinklerforum
You never can tell when office workers will be storing a thousand gallons of flammable methyl ethyl death floor to ceiling in styrofoam containers. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter

Re: mattress storage

2020-06-05 Thread Ron Greenman via Sprinklerforum
When it comes to high hazard furnishings I always ask, "What would IKEA do?" Giant buildings full of plastic and kindling. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film direct

Re: Structural Load

2020-06-03 Thread Ron Greenman via Sprinklerforum
or dead loads, including the sprinkler system. And I'm guessing that in California insufficient point loading for hanging would the least of your concerns regarding structure. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence o

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Ron Greenman via Sprinklerforum
agree that the intent is met when using flex drops but since there is no stated exception it is now enforcing the letter because that's the mandate, or even merely a CYA. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man.

Dust Collection

2020-05-22 Thread Ron Greenman via Sprinklerforum
Does anyone know the NFPA references for dust ducting and collection for compressed paper laminate production? I am home (of course) and my books are 75 miles away. Thanks. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner

Re: [External] Re: I-B construction - ABS plumbing piping

2020-05-21 Thread Ron Greenman via Sprinklerforum
h the electrical or alarm or data or some sparky contractor. If adding sprinklers is just the band-aid for a problem that shouldn't have been allowed to exist in the first place... Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of ma

Re: Air Venting

2020-03-06 Thread Ron Greenman via Sprinklerforum
When say sprigs do you mean the sprinklers are on sprigs as defined in 13 or do you mean the branch lines are are of risers that some folks sometimes call sprigs? And as a fun FYI for everyone, autocorrupt changed sprigs to spirirs in one place, springs in another, and sprints in another. On Fri,

3000 sqft rule

2020-03-04 Thread Ron Greenman via Sprinklerforum
Does anyone know what edition of 13 the 3000 sqft rule was introduced? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942

Re: Combustible dust collector

2020-02-24 Thread Ron Greenman via Sprinklerforum
ow every bit of Skyler's advice on this matter. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Mon, Feb 24, 2020 at 7:46 AM Dewayne Martine

Re: TYCO RM-1

2020-02-09 Thread Ron Greenman via Sprinklerforum
That sounds like the real number to me. On Sun, Feb 9, 2020 at 11:06 AM Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum wrote: > *That is what I have always used. Just friction loss through length plus > the 3 psi.* > > > > [image: MFP_logo_F] > > Travis Mack

Re: Hazard Group?

2019-12-17 Thread Ron Greenman via Sprinklerforum
I'm presuming the gas in appropriate containers in an appropriate cabinet, although at the school where I worked the maintenance guys would leave the gas cans outside or on top of the cabinets. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent t

Re: Detached Garage

2019-12-06 Thread Ron Greenman via Sprinklerforum
number of cars that can fit in it. Other jurisdictions have varying rules regarding densities, sprinkler location, and whether the garage needs to be fully covered or partially covered. Often these requirements are codified and applied uniformly and sometimes they aren't. Ron Gre

Re: [EXTERNAL] Not required, requirement

2019-11-19 Thread Ron Greenman via Sprinklerforum
roved by the overseers of the utility district and depending on the laws of your state, you may have already lost the battle. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author,

Re: Existing Dry system testing- chapter 25

2019-11-13 Thread Ron Greenman via Sprinklerforum
Doesn't 13-13 25.2.1.6 exempt "Just you [sic] basic arm-over relocates." from a hydrostatic test above system working pressure? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film d

Re: Hotel washroom & closets

2019-10-15 Thread Ron Greenman via Sprinklerforum
I’m trying to figure out how length of stay would effect the fire hazard. On Tue, Oct 15, 2019 at 6:02 PM Bruce Verhei via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > We had an Extended Stay America that had commonly had units rented long > term. It was a hotel for our purpo

Re: Upright Sprinkler

2019-10-08 Thread Ron Greenman via Sprinklerforum
ion eliminates the obstruction or limits the impact of the obstruction caused by the branch line so that it does not pose a significant problem. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film direc

Re: [EXTERNAL] FW: Dry Pipe Valve to Wet

2019-09-24 Thread Ron Greenman via Sprinklerforum
only encountered in dry systems would be eliminated. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Tue, Sep 24, 2019 at 1:00 PM Michael Hill

Re: [EXTERNAL] FW: Dry Pipe Valve to Wet

2019-09-24 Thread Ron Greenman via Sprinklerforum
line, have the holes plugged, and have it marked as no longer being any kind of valve? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Tue, Sep

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Ron Greenman via Sprinklerforum
I like this discussion. What about the dreaded perimeter opening 9n an otherwise non-combustible ceiling? Does a spacing ruling from the opening apply? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter

Re: N1.85 graph paper

2019-08-28 Thread Ron Greenman via Sprinklerforum
Hey Travis. Everything good out there for you? Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Wed, Aug 28, 2019 at 2:32 PM Travis Allen

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Ron Greenman via Sprinklerforum
ons per 25 only had to be made from the floor (or that's what he meant 🙊), but Scott makes some good points about the difficulty that might be encountered for other activities. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man.

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Ron Greenman via Sprinklerforum
Do note that NFPA 13 requires that the locations of low point drains be identified on the "General Information Sign" as well as the drain itself. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwr

Re: Captive Aire Systems

2019-08-15 Thread Ron Greenman via Sprinklerforum
ociation of Plumbing and Mechanical Officials (IAPMO): Installation, Material and Property Standard PS 108-98 – Grease Fire Suppression Systems. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film dir

Re: CBC / CFC vs NFPA 13

2019-07-24 Thread Ron Greenman
Scot. I've lost your email. Mine has not changed. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Wed, Jul 24, 2019 at 9:56

Re: Hazard

2019-07-03 Thread Ron Greenman
In addition to Travis’ comment if you don’t have an engineer define the occupancy and hazard you may need a long chat with the FM, the building/zoning folks and the owner. On Wed, Jul 3, 2019 at 9:47 AM Travis Mack, SET, CFPS, CWBSP, RME-G < tm...@mfpdesign.com> wrote: > > > *Owner information ce

Re: Multi-Level Ducts

2019-07-02 Thread Ron Greenman
And before we go off on a "that's crazy" line of postings regarding my previous post: I know. It's crazy thinking. But it complies with the rules. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog

Re: Multi-Level Ducts

2019-07-02 Thread Ron Greenman
sprinkler under them. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Tue, Jul 2, 2019 at 10:52 AM Sean.VanGaal wrote: > I want to switch t

Re: Where to fine lowest mean temp info

2019-06-28 Thread Ron Greenman
If you’re looking for lowest mean go here and replace tacoma, wa with the city you want. https://www.weather-us.com/en/washington-usa/tacoma-climate On Fri, Jun 28, 2019 at 3:15 PM Ben Young wrote: > I can't figure out how to get 'here' for other regions, but this data is > kind of what I'm lo

Re: Attic sprinklers

2019-06-28 Thread Ron Greenman
*From the ICC:* *ATTIC*. ... In order to fully clarify that portion of a building *defined*as an *attic*, Section 202 identifies an *attic* as that space between the ceiling beams at the top story and the roof rafters. An *attic*designation is appropriate only if the area is not considered occupiab

Re: [EXTERNAL] Welded outlets - Equivalent feet

2019-06-26 Thread Ron Greenman
https://www.engineersedge.com/fluid_flow/fluid_flow_table_content.htm Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Wed, Jun 26, 2019 at

Re: Outer Obstructions @ Porte-Cocheres

2019-06-24 Thread Ron Greenman
27;t been keeping up with changes well as i could (should?). Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Mon, Jun 24, 2019 at 3:24 PM

Re: Bags to Protect Sprinklers from Overspray

2019-06-13 Thread Ron Greenman
https://www.nashvillewraps.com/cellophane/biodegradable-bags/p-54 Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Thu, Jun 13, 2019 at 11

Re: Ammo Production

2019-06-08 Thread Ron Greenman
an ultra high speed deluge system (1/200th of a second or less from detection to water application) in a darkened area with light safe entries, and spark detectors everywhere. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of

  1   2   3   4   5   6   7   8   9   10   >