2009-08-13 Thread John Thomas
Unless your equipment is tolerant of voltage swings, you will still 
probably want a DC-DC regulator, but that will likely be more efficient 
than a 12/24volt to 120 volt inverter.

John


Leon D. Zetekoff, NCE wrote:
> Hi Guys...I'd steer away from inverters since they soak up a lot of 
> power. You might want to look at some solar stuff with some of the AGM 
> batteries Marlon mentioned in another thread. Run everything @ 24V is 
> good that way you don't need any dc-dc converters.
>
> Leon
>
> * os10ru...@gmail.com wrote, On 8/2/2009 3:27 PM:
>> You might want something like an inverter (Xantrex for example) 
>> which  includes a DC to AC inverter, battery charger, and automatic 
>> transfer  switch. Add the batteries and you're done.
>>
>> Greg
>>
>> On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:
>>
>>  
>>> Thank you,
>>> That is very good advice. After some research, I'm leaning toward a  
>>> UPS.
>>>
>>> A pair of good AGM batteries and charge controller will cost less  
>>> and be far less maintainence. Then I'd just run the CMM off the  
>>> batteries @ 24VDC.
>>>
>>> Thanks again
>>> Jerry
>>>
>>>
>>> -Original Message-----
>>> From: wireless-boun...@wispa.org 
>>> [mailto:wireless-boun...@wispa.org]  On Behalf Of Gary Garrett
>>> Sent: Sunday, August 02, 2009 11:59 AM
>>> To: WISPA General List
>>> Subject: Re: [WISPA] Small auto start generator
>>>
>>> Small generators do not auto start very reliably.
>>> When cold or dampness causes hard starting the starter can overheat  
>>> and
>>> burn out. Generally you need an electric choke to start gas engines,
>>> propane can "flood" and need to rest before trying again, diesel 
>>> can  be
>>> REAL hard to start when cold. Auto starters can not adapt to changing
>>> conditions.
>>> Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase.  
>>> (1955
>>> Model)
>>> The monitor cranks for 1 min then rests and tries 3 times.  
>>> Everything is
>>> adjustable. It knows to stop cranking when it sees AC voltage from the
>>> Gen. so the motor over runs the starter for just a few seconds. Only a
>>> huge starter motor can take this abuse and last unattended.
>>>
>>> You may be money ahead to find out why the existing generator is not
>>> starting and get it fixed.
>>>
>>> Jerry Richardson wrote:
>>>
>>>> We rent on a tower that is suspposed to have gen-set backup but it  
>>>> does not start reliably.
>>>>
>>>> Any recommendations on a small auto-start generator? We only need  
>>>> to power a CMMmicro - ~100watts.
>>>>
>>>> Thanks
>>>>
>>>> __
>>>> Jerry Richardson
>>>> airCloud Communications
>>>>   
> 
>
>
> No virus found in this outgoing message.
> Checked by AVG - www.avg.com 
> Version: 8.5.406 / Virus Database: 270.13.42/2278 - Release Date: 08/02/09 
> 17:56:00
>   
> 
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-13 Thread John Thomas
Is this some place you could put some batteries and a solar panel or 
small windmill?

John


Jerry Richardson wrote:
> Thank you,
> That is very good advice. After some research, I'm leaning toward a UPS. 
>
> A pair of good AGM batteries and charge controller will cost less and be far 
> less maintainence. Then I'd just run the CMM off the batteries @ 24VDC.
>
> Thanks again
> Jerry
>
>
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On 
> Behalf Of Gary Garrett
> Sent: Sunday, August 02, 2009 11:59 AM
> To: WISPA General List
> Subject: Re: [WISPA] Small auto start generator
>
> Small generators do not auto start very reliably.
> When cold or dampness causes hard starting the starter can overheat and 
> burn out. Generally you need an electric choke to start gas engines, 
> propane can "flood" and need to rest before trying again, diesel can be 
> REAL hard to start when cold. Auto starters can not adapt to changing 
> conditions.
> Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955 
> Model)
> The monitor cranks for 1 min then rests and tries 3 times. Everything is 
> adjustable. It knows to stop cranking when it sees AC voltage from the 
> Gen. so the motor over runs the starter for just a few seconds. Only a 
> huge starter motor can take this abuse and last unattended.
>
> You may be money ahead to find out why the existing generator is not 
> starting and get it fixed.
>
> Jerry Richardson wrote:
>   
>> We rent on a tower that is suspposed to have gen-set backup but it does not 
>> start reliably.
>>
>> Any recommendations on a small auto-start generator? We only need to power a 
>> CMMmicro - ~100watts.
>>
>> Thanks
>>
>>
>>
>> __
>> Jerry Richardson
>> airCloud Communications
>>
>>
>>
>>
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> 
>>  
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>> 
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
>   




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-06 Thread Curtis Maurand
I don't remember, you'd have to call them.

--C

3-dB Networks wrote:
> What do those cost?
>
> Daniel White
> 3-dB Networks
> http://www.3dbnetworks.com
>
>
>   
>> -Original Message-
>> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
>> Behalf Of Curtis Maurand
>> Sent: Thursday, August 06, 2009 8:08 AM
>> To: WISPA General List
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>> Something like that.  These guys have one that runs for 90 hours is 250
>> watts 12 or 24 VDC and uses a methanol and water mix.  methane fuel
>> cells don't use platinum and are, therefore, less expensive.  Its
>> configurable with an RS-232 port.  It can be used as a battery charger
>> as well so that if your system has dropped to battery, it will recharge
>> the battery after its charge has dropped to a configurable level.  Its
>> pretty cool stuff.  I was looking to  backup power an entire data center
>> with one of the larger ones a couple of years ago.  There is a european
>> company called BAXI that makes fuel cells as well.   This one is perfect
>> for the application requirements in the original email.  I don't recall
>> them as being that expensive either.
>>
>>
>> http://www.idatech.com/Products-and-Services-iGen-System2.asp
>>
>>
>> --Curtis
>>
>> Tom DeReggi wrote:
>> 
>>> Thanks
>>>
>>> PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X
>>>   
>> billion
>> 
>>> grant to pioneer?
>>>
>>> Tom DeReggi
>>> RapidDSL & Wireless, Inc
>>> IntAirNet- Fixed Wireless Broadband
>>>
>>>
>>> - Original Message -
>>> From: "Curtis Maurand" 
>>> To: "WISPA General List" 
>>> Sent: Tuesday, August 04, 2009 3:14 PM
>>> Subject: Re: [WISPA] Small auto start generator
>>>
>>>
>>>
>>>   
>>>> Sorry, I should have posted this page.
>>>>
>>>> no moving parts.
>>>>
>>>> http://www.idatech.com/
>>>>
>>>>
>>>>
>>>> Tom DeReggi wrote:
>>>>
>>>> 
>>>>> Patrick,
>>>>>
>>>>> All excellent points, and reality checks. Thanks for the feedback!
>>>>>
>>>>>
>>>>> Tom DeReggi
>>>>> RapidDSL & Wireless, Inc
>>>>> IntAirNet- Fixed Wireless Broadband
>>>>>
>>>>>
>>>>> - Original Message -
>>>>> From: "Patrick Shoemaker" 
>>>>> To: "WISPA General List" 
>>>>> Sent: Monday, August 03, 2009 5:58 PM
>>>>> Subject: Re: [WISPA] Small auto start generator
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>   
>>>>>> I think you'll find that to get a propane/NG generator installed on
>>>>>> 
>> a
>> 
>>>>>> commercial building rooftop, you'll be looking at $10k minimum
>>>>>> 
>> using
>> 
>>>>>> even the cheapest Generac air-cooled units. You'll need a roofing
>>>>>> company to come out and modify the roof to provide a mounting
>>>>>> 
>> surface
>> 
>>>>>> for the generator, that will probably be the biggest cost. Getting
>>>>>> management comfortable with modifying a $300k roof membrane could
>>>>>> 
>> be an
>> 
>>>>>> issue as well. Then getting gas to the unit from the building's gas
>>>>>> supply will require a plumbing contractor, permits, inspections.
>>>>>> 
>> Then
>> 
>>>>>> the electrical hookup- more permits and inspections and a licensed
>>>>>> 
>> EC.
>> 
>>>>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new
>>>>>> 
>> site:
>> 
>>>>>> $1500 including shipping.
>>>>>>
>>>>>> A note on the Generac air-cooled generators. They break. All
>>>>>> 
>> generators
>> 
>>>>>> break. The key is routine testing and PM. The generac air-cooled
>>>

Re: [WISPA] Small auto start generator

2009-08-06 Thread Gino Villarini
Any ballpark figures?> 


Gino A. Villarini
g...@aeronetpr.com
Aeronet Wireless Broadband Corp.
tel  787.273.4143   fax   787.273.4145

-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Curtis Maurand
Sent: Thursday, August 06, 2009 11:08 AM
To: WISPA General List
Subject: Re: [WISPA] Small auto start generator


Something like that.  These guys have one that runs for 90 hours is 250
watts 12 or 24 VDC and uses a methanol and water mix.  methane fuel
cells don't use platinum and are, therefore, less expensive.  Its
configurable with an RS-232 port.  It can be used as a battery charger
as well so that if your system has dropped to battery, it will recharge
the battery after its charge has dropped to a configurable level.  Its
pretty cool stuff.  I was looking to  backup power an entire data center
with one of the larger ones a couple of years ago.  There is a european 
company called BAXI that makes fuel cells as well.   This one is perfect

for the application requirements in the original email.  I don't recall
them as being that expensive either.


http://www.idatech.com/Products-and-Services-iGen-System2.asp


--Curtis

Tom DeReggi wrote:
> Thanks
>
> PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X 
> billion grant to pioneer?
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message -
> From: "Curtis Maurand" 
> To: "WISPA General List" 
> Sent: Tuesday, August 04, 2009 3:14 PM
> Subject: Re: [WISPA] Small auto start generator
>
>
>   
>> Sorry, I should have posted this page.
>>
>> no moving parts.
>>
>> http://www.idatech.com/
>>
>>
>>
>> Tom DeReggi wrote:
>> 
>>> Patrick,
>>>
>>> All excellent points, and reality checks. Thanks for the feedback!
>>>
>>>
>>> Tom DeReggi
>>> RapidDSL & Wireless, Inc
>>> IntAirNet- Fixed Wireless Broadband
>>>
>>>
>>> - Original Message -
>>> From: "Patrick Shoemaker" 
>>> To: "WISPA General List" 
>>> Sent: Monday, August 03, 2009 5:58 PM
>>> Subject: Re: [WISPA] Small auto start generator
>>>
>>>
>>>
>>>   
>>>> I think you'll find that to get a propane/NG generator installed on

>>>> a commercial building rooftop, you'll be looking at $10k minimum 
>>>> using even the cheapest Generac air-cooled units. You'll need a 
>>>> roofing company to come out and modify the roof to provide a 
>>>> mounting surface for the generator, that will probably be the 
>>>> biggest cost. Getting management comfortable with modifying a $300k

>>>> roof membrane could be an issue as well. Then getting gas to the 
>>>> unit from the building's gas supply will require a plumbing 
>>>> contractor, permits, inspections. Then the electrical hookup- more
permits and inspections and a licensed EC.
>>>>
>>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new
site:
>>>> $1500 including shipping.
>>>>
>>>> A note on the Generac air-cooled generators. They break. All 
>>>> generators break. The key is routine testing and PM. The generac 
>>>> air-cooled models don't have any provision for automatic alarm 
>>>> reporting. So when a battery dies or gas valve sticks or spark plug

>>>> fouls or whatever, you won't know about it until a manual site 
>>>> inspection or the power goes out. The better generators (and the 
>>>> Generac liquid cooled models) have contact closures or RS232 
>>>> interfaces to report these conditions to your site monitoring
system, in turn notifying you back at the NOC.
>>>>
>>>>
>>>> Patrick Shoemaker
>>>> Vector Data Systems LLC
>>>> shoemak...@vectordatasystems.com
>>>> office: (301) 358-1690 x36
>>>> http://www.vectordatasystems.com
>>>>
>>>>
>>>> Tom DeReggi wrote:
>>>>
>>>> 
>>>>> We also use the triplite APS inverters with good quality Gel cell.
>>>>> Actually,
>>>>> we got a good 15 years out of the existing C&D batteries, because 
>>>>> we inherited them from Teligent days :-) But new, qty 4- 12V 150AH

>>>>> batteries in series for about 3500watt and decent run-time is 
>>>>> $1400. + $800 for replacement inverters.  (The Triplites worked 

Re: [WISPA] Small auto start generator

2009-08-06 Thread Chuck Profito
I called one of the resellers, $5-10k DEPENDING ON CONFIGURATION AND FUEL.
I think an extra 8D at $205 would be more reliable and biannual replacement
would pencil better...But they are COOL, and very small.  At least that 250w
unit is.
cp
-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of 3-dB Networks
Sent: Thursday, August 06, 2009 8:11 AM
To: 'WISPA General List'
Subject: Re: [WISPA] Small auto start generator

What do those cost?

Daniel White
3-dB Networks
http://www.3dbnetworks.com


>-Original Message-
>From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
>Behalf Of Curtis Maurand
>Sent: Thursday, August 06, 2009 8:08 AM
>To: WISPA General List
>Subject: Re: [WISPA] Small auto start generator
>
>
>Something like that.  These guys have one that runs for 90 hours is 250
>watts 12 or 24 VDC and uses a methanol and water mix.  methane fuel
>cells don't use platinum and are, therefore, less expensive.  Its
>configurable with an RS-232 port.  It can be used as a battery charger
>as well so that if your system has dropped to battery, it will recharge
>the battery after its charge has dropped to a configurable level.  Its
>pretty cool stuff.  I was looking to  backup power an entire data center
>with one of the larger ones a couple of years ago.  There is a european
>company called BAXI that makes fuel cells as well.   This one is perfect
>for the application requirements in the original email.  I don't recall
>them as being that expensive either.
>
>
>http://www.idatech.com/Products-and-Services-iGen-System2.asp
>
>
>--Curtis
>
>Tom DeReggi wrote:
>> Thanks
>>
>> PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X
>billion
>> grant to pioneer?
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message -
>> From: "Curtis Maurand" 
>> To: "WISPA General List" 
>> Sent: Tuesday, August 04, 2009 3:14 PM
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>>
>>> Sorry, I should have posted this page.
>>>
>>> no moving parts.
>>>
>>> http://www.idatech.com/
>>>
>>>
>>>
>>> Tom DeReggi wrote:
>>>
>>>> Patrick,
>>>>
>>>> All excellent points, and reality checks. Thanks for the feedback!
>>>>
>>>>
>>>> Tom DeReggi
>>>> RapidDSL & Wireless, Inc
>>>> IntAirNet- Fixed Wireless Broadband
>>>>
>>>>
>>>> - Original Message -
>>>> From: "Patrick Shoemaker" 
>>>> To: "WISPA General List" 
>>>> Sent: Monday, August 03, 2009 5:58 PM
>>>> Subject: Re: [WISPA] Small auto start generator
>>>>
>>>>
>>>>
>>>>
>>>>> I think you'll find that to get a propane/NG generator installed on
>a
>>>>> commercial building rooftop, you'll be looking at $10k minimum
>using
>>>>> even the cheapest Generac air-cooled units. You'll need a roofing
>>>>> company to come out and modify the roof to provide a mounting
>surface
>>>>> for the generator, that will probably be the biggest cost. Getting
>>>>> management comfortable with modifying a $300k roof membrane could
>be an
>>>>> issue as well. Then getting gas to the unit from the building's gas
>>>>> supply will require a plumbing contractor, permits, inspections.
>Then
>>>>> the electrical hookup- more permits and inspections and a licensed
>EC.
>>>>>
>>>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new
>site:
>>>>> $1500 including shipping.
>>>>>
>>>>> A note on the Generac air-cooled generators. They break. All
>generators
>>>>> break. The key is routine testing and PM. The generac air-cooled
>models
>>>>> don't have any provision for automatic alarm reporting. So when a
>>>>> battery dies or gas valve sticks or spark plug fouls or whatever,
>you
>>>>> won't know about it until a manual site inspection or the power
>goes
>>>>> out. The better generators (and the Generac liquid cooled models)
>have
>>>>> contact closures or RS232 interfaces to report these conditions to
>your
>>>>> site monitoring system, in turn notifying you back at the NOC.

Re: [WISPA] Small auto start generator

2009-08-06 Thread 3-dB Networks
What do those cost?

Daniel White
3-dB Networks
http://www.3dbnetworks.com


>-Original Message-
>From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
>Behalf Of Curtis Maurand
>Sent: Thursday, August 06, 2009 8:08 AM
>To: WISPA General List
>Subject: Re: [WISPA] Small auto start generator
>
>
>Something like that.  These guys have one that runs for 90 hours is 250
>watts 12 or 24 VDC and uses a methanol and water mix.  methane fuel
>cells don't use platinum and are, therefore, less expensive.  Its
>configurable with an RS-232 port.  It can be used as a battery charger
>as well so that if your system has dropped to battery, it will recharge
>the battery after its charge has dropped to a configurable level.  Its
>pretty cool stuff.  I was looking to  backup power an entire data center
>with one of the larger ones a couple of years ago.  There is a european
>company called BAXI that makes fuel cells as well.   This one is perfect
>for the application requirements in the original email.  I don't recall
>them as being that expensive either.
>
>
>http://www.idatech.com/Products-and-Services-iGen-System2.asp
>
>
>--Curtis
>
>Tom DeReggi wrote:
>> Thanks
>>
>> PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X
>billion
>> grant to pioneer?
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message -
>> From: "Curtis Maurand" 
>> To: "WISPA General List" 
>> Sent: Tuesday, August 04, 2009 3:14 PM
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>>
>>> Sorry, I should have posted this page.
>>>
>>> no moving parts.
>>>
>>> http://www.idatech.com/
>>>
>>>
>>>
>>> Tom DeReggi wrote:
>>>
>>>> Patrick,
>>>>
>>>> All excellent points, and reality checks. Thanks for the feedback!
>>>>
>>>>
>>>> Tom DeReggi
>>>> RapidDSL & Wireless, Inc
>>>> IntAirNet- Fixed Wireless Broadband
>>>>
>>>>
>>>> - Original Message -
>>>> From: "Patrick Shoemaker" 
>>>> To: "WISPA General List" 
>>>> Sent: Monday, August 03, 2009 5:58 PM
>>>> Subject: Re: [WISPA] Small auto start generator
>>>>
>>>>
>>>>
>>>>
>>>>> I think you'll find that to get a propane/NG generator installed on
>a
>>>>> commercial building rooftop, you'll be looking at $10k minimum
>using
>>>>> even the cheapest Generac air-cooled units. You'll need a roofing
>>>>> company to come out and modify the roof to provide a mounting
>surface
>>>>> for the generator, that will probably be the biggest cost. Getting
>>>>> management comfortable with modifying a $300k roof membrane could
>be an
>>>>> issue as well. Then getting gas to the unit from the building's gas
>>>>> supply will require a plumbing contractor, permits, inspections.
>Then
>>>>> the electrical hookup- more permits and inspections and a licensed
>EC.
>>>>>
>>>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new
>site:
>>>>> $1500 including shipping.
>>>>>
>>>>> A note on the Generac air-cooled generators. They break. All
>generators
>>>>> break. The key is routine testing and PM. The generac air-cooled
>models
>>>>> don't have any provision for automatic alarm reporting. So when a
>>>>> battery dies or gas valve sticks or spark plug fouls or whatever,
>you
>>>>> won't know about it until a manual site inspection or the power
>goes
>>>>> out. The better generators (and the Generac liquid cooled models)
>have
>>>>> contact closures or RS232 interfaces to report these conditions to
>your
>>>>> site monitoring system, in turn notifying you back at the NOC.
>>>>>
>>>>>
>>>>> Patrick Shoemaker
>>>>> Vector Data Systems LLC
>>>>> shoemak...@vectordatasystems.com
>>>>> office: (301) 358-1690 x36
>>>>> http://www.vectordatasystems.com
>>>>>
>>>>>
>>>>> Tom DeReggi wrote:
>>>>>
>>>>>
>>>>>> We also use the triplite APS inverters with good quality Gel cel

Re: [WISPA] Small auto start generator

2009-08-06 Thread Curtis Maurand

Something like that.  These guys have one that runs for 90 hours is 250 
watts 12 or 24 VDC and uses a methanol and water mix.  methane fuel 
cells don't use platinum and are, therefore, less expensive.  Its 
configurable with an RS-232 port.  It can be used as a battery charger 
as well so that if your system has dropped to battery, it will recharge 
the battery after its charge has dropped to a configurable level.  Its 
pretty cool stuff.  I was looking to  backup power an entire data center 
with one of the larger ones a couple of years ago.  There is a european 
company called BAXI that makes fuel cells as well.   This one is perfect 
for the application requirements in the original email.  I don't recall 
them as being that expensive either.


http://www.idatech.com/Products-and-Services-iGen-System2.asp


--Curtis

Tom DeReggi wrote:
> Thanks
>
> PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X billion 
> grant to pioneer?
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message - 
> From: "Curtis Maurand" 
> To: "WISPA General List" 
> Sent: Tuesday, August 04, 2009 3:14 PM
> Subject: Re: [WISPA] Small auto start generator
>
>
>   
>> Sorry, I should have posted this page.
>>
>> no moving parts.
>>
>> http://www.idatech.com/
>>
>>
>>
>> Tom DeReggi wrote:
>> 
>>> Patrick,
>>>
>>> All excellent points, and reality checks. Thanks for the feedback!
>>>
>>>
>>> Tom DeReggi
>>> RapidDSL & Wireless, Inc
>>> IntAirNet- Fixed Wireless Broadband
>>>
>>>
>>> - Original Message - 
>>> From: "Patrick Shoemaker" 
>>> To: "WISPA General List" 
>>> Sent: Monday, August 03, 2009 5:58 PM
>>> Subject: Re: [WISPA] Small auto start generator
>>>
>>>
>>>
>>>   
>>>> I think you'll find that to get a propane/NG generator installed on a
>>>> commercial building rooftop, you'll be looking at $10k minimum using
>>>> even the cheapest Generac air-cooled units. You'll need a roofing
>>>> company to come out and modify the roof to provide a mounting surface
>>>> for the generator, that will probably be the biggest cost. Getting
>>>> management comfortable with modifying a $300k roof membrane could be an
>>>> issue as well. Then getting gas to the unit from the building's gas
>>>> supply will require a plumbing contractor, permits, inspections. Then
>>>> the electrical hookup- more permits and inspections and a licensed EC.
>>>>
>>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new site:
>>>> $1500 including shipping.
>>>>
>>>> A note on the Generac air-cooled generators. They break. All generators
>>>> break. The key is routine testing and PM. The generac air-cooled models
>>>> don't have any provision for automatic alarm reporting. So when a
>>>> battery dies or gas valve sticks or spark plug fouls or whatever, you
>>>> won't know about it until a manual site inspection or the power goes
>>>> out. The better generators (and the Generac liquid cooled models) have
>>>> contact closures or RS232 interfaces to report these conditions to your
>>>> site monitoring system, in turn notifying you back at the NOC.
>>>>
>>>>
>>>> Patrick Shoemaker
>>>> Vector Data Systems LLC
>>>> shoemak...@vectordatasystems.com
>>>> office: (301) 358-1690 x36
>>>> http://www.vectordatasystems.com
>>>>
>>>>
>>>> Tom DeReggi wrote:
>>>>
>>>> 
>>>>> We also use the triplite APS inverters with good quality Gel cell.
>>>>> Actually,
>>>>> we got a good 15 years out of the existing C&D batteries, because we
>>>>> inherited them from Teligent days :-)
>>>>> But new, qty 4- 12V 150AH batteries in series for about 3500watt and
>>>>> decent
>>>>> run-time is $1400. + $800 for replacement inverters.  (The Triplites
>>>>> worked
>>>>> really well, but about half of them died by the end of eight years. We
>>>>> matched good inverters with good pre-existing batteries and vice 
>>>>> versa.)
>>>>> So
>>>>> our thought was Why not buy a $2000 generator for the run-time and
>>>>&g

Re: [WISPA] Small auto start generator

2009-08-04 Thread Tom DeReggi
Thanks

PS. Isn't Hydrogen Fual Cell the technology Spring just got like $X billion 
grant to pioneer?

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Curtis Maurand" 
To: "WISPA General List" 
Sent: Tuesday, August 04, 2009 3:14 PM
Subject: Re: [WISPA] Small auto start generator


>
> Sorry, I should have posted this page.
>
> no moving parts.
>
> http://www.idatech.com/
>
>
>
> Tom DeReggi wrote:
>> Patrick,
>>
>> All excellent points, and reality checks. Thanks for the feedback!
>>
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message ----- 
>> From: "Patrick Shoemaker" 
>> To: "WISPA General List" 
>> Sent: Monday, August 03, 2009 5:58 PM
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>>
>>> I think you'll find that to get a propane/NG generator installed on a
>>> commercial building rooftop, you'll be looking at $10k minimum using
>>> even the cheapest Generac air-cooled units. You'll need a roofing
>>> company to come out and modify the roof to provide a mounting surface
>>> for the generator, that will probably be the biggest cost. Getting
>>> management comfortable with modifying a $300k roof membrane could be an
>>> issue as well. Then getting gas to the unit from the building's gas
>>> supply will require a plumbing contractor, permits, inspections. Then
>>> the electrical hookup- more permits and inspections and a licensed EC.
>>>
>>> I just got a quote for qty 8 110AH 12v AGM batteries for a new site:
>>> $1500 including shipping.
>>>
>>> A note on the Generac air-cooled generators. They break. All generators
>>> break. The key is routine testing and PM. The generac air-cooled models
>>> don't have any provision for automatic alarm reporting. So when a
>>> battery dies or gas valve sticks or spark plug fouls or whatever, you
>>> won't know about it until a manual site inspection or the power goes
>>> out. The better generators (and the Generac liquid cooled models) have
>>> contact closures or RS232 interfaces to report these conditions to your
>>> site monitoring system, in turn notifying you back at the NOC.
>>>
>>>
>>> Patrick Shoemaker
>>> Vector Data Systems LLC
>>> shoemak...@vectordatasystems.com
>>> office: (301) 358-1690 x36
>>> http://www.vectordatasystems.com
>>>
>>>
>>> Tom DeReggi wrote:
>>>
>>>> We also use the triplite APS inverters with good quality Gel cell.
>>>> Actually,
>>>> we got a good 15 years out of the existing C&D batteries, because we
>>>> inherited them from Teligent days :-)
>>>> But new, qty 4- 12V 150AH batteries in series for about 3500watt and
>>>> decent
>>>> run-time is $1400. + $800 for replacement inverters.  (The Triplites
>>>> worked
>>>> really well, but about half of them died by the end of eight years. We
>>>> matched good inverters with good pre-existing batteries and vice 
>>>> versa.)
>>>> So
>>>> our thought was Why not buy a $2000 generator for the run-time and
>>>> load,
>>>> and then several smaller UPSes for infront to cover the surges, power
>>>> conditioning, and monitoring? Ones that keep running even when 
>>>> batteries
>>>> short out.  Part of the reason we are investigating is that we now have
>>>> duplicate need of devices to power.  Some are AC devices like PC 
>>>> routers.
>>>> Some are 20-24VDC w/AC adapters. Some are new licensed gear running on
>>>> 48V.
>>>> Cost is increased having long battery run time on both seperate AC and 
>>>> DC
>>>> backup power subsystems. And how do we plan for load growth? How many 
>>>> new
>>>> radios installed will be AC or DC? Unlicensed versus Licensed? We 
>>>> really
>>>> dont know in advance.  There is a lot of power waste going from AC to 
>>>> DC
>>>> to
>>>> AC to DC.
>>>>
>>>> The thought was... If long run time was accomplished by the propaine
>>>> generator, both DC and AC battery subsystems could be installed with
>>>> lower
>>>> cost lower run-time batteries.  We'd still need to account for 

Re: [WISPA] Small auto start generator

2009-08-04 Thread jp
http://en.wikipedia.org/wiki/Radioisotope_thermoelectric_generator

The soviets made portable radioactive generators to power lighthouses 
and beacons; 87 years and you've only used half your fuel.

On Tue, Aug 04, 2009 at 11:19:31AM -0700, Chuck Profito wrote:
> Let's not forget small nuclear power as sold in 1951! ... http://xrl.in/2u36
> 
> 
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
> Behalf Of Curtis Maurand
> Sent: Tuesday, August 04, 2009 10:39 AM
> To: WISPA General List
> Subject: Re: [WISPA] Small auto start generator
> 
> 
> Fuel cells, too.
> 
> http://www.fuelcellmarkets.com/products_and_services/3,1,599,17,7561.html
> 
> 
> 
> Christopher Erickson wrote:
> > The right type of batteries could give you 15 to 20 years of service.
> >
> > And adding a pair of solar panels and an MPPT solar charge controller
> could
> > increase your backup battery run time from a couple of days to a couple
> > of weeks.  And no volatile fuel issues to deal with either.  And their PMI
> > interval is a godsend too.  And cheaper than a genny.
> >
> > Add another panel or two and you might even be able to drop your grid
> > connection.
> >
> > Remember to eliminate as many power conversions as possible from your
> > telecom power design.
> >
> > -Christopher Erickson
> > Network Design Engineer
> > 5432 E. Northern Lights Blvd., Suite 529
> > Anchorage, AK 99508
> > N61?11.710' W149?46.723'
> >
> >
> >   
> >> -Original Message-
> >> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]on
> >> Behalf Of Tom DeReggi
> >> Sent: Monday, August 03, 2009 10:49 AM
> >> To: WISPA General List
> >> Subject: Re: [WISPA] Small auto start generator
> >>
> >>
> >> Patrick,
> >>
> >> In general, sounds like good advice.
> >>
> >> To clarify our intent, in posting.
> >>
> >> >From yr 2000-2008, our model was to
> >>
> >> 1) Have minimum 12 hour run-time of battery for core cell sites.
> >> 2) Have contingency plan for hooking up a mobile gasoline powered
> >> generator,
> >> in longer lasting Emergencies.
> >> (We have a couple hot spare generators)
> >>
> >> Why are we changing our view point?
> >>
> >> 1) Many of the batteries have now died, and need replaced. Batteries are
> >> still very expensive. Propaine Generators have come way down in
> >> price (aka
> >> Generac) In most case, the generator will be less expensive than the
> >> batteries, based on watt load at the sites.
> >>
> >> 2) Our network has grown, but our staff size has shrunk. We realize the
> >> challenge that more than one site can loose power at once, and
> >> harder to get
> >> to multiple locations at once with generators.
> >> Its hard to know when batteries will hold or not, when
> >> towards the end
> >> of their life, so its always a rush with the genrators. 9/10 cases by the
> >> time we get generators onsite, the power gets restored within minutes.
> >>
> >> 3)  Its easy to throw a generator on a Grant Application :-)
> >>
> >> We believe permanent onsite generators would likely increase
> >> uptime, and not
> >> necessarilly be more expensive, for some of our sites. (We'd of
> >> course still
> >> keep some patteries inline) The question is whether it will be
> >> more hassle
> >> than we realize to re-fill them and inspect them. Some people told me
> >> quarterly inspections are needed, or sometimes they do not start when
> >> needed.
> >>
> >> We are already connected to building generators, where we were
> >> allowed to,
> >> so we are looking at sites where our only option was to put in our own.
> >> I'm still uncertain what objections or preferences property
> >> management would
> >> have for this type stuff.  For example, whether they would be concerned
> >> about it blowing up if a gas leak occured.
> >>
> >> I actually have one building in mind wher egetting a new electrical
> >> connector from the roof to the ground would be really a big pain. Would
> >> require Xray and drilling every floor of 20.
> >> There I'd like to put a roof mounted propaine generator. I was thinking
> >> maybe the best option is to just have a small external tank, and swap the
> &g

Re: [WISPA] Small auto start generator

2009-08-04 Thread Curtis Maurand

Sorry, I should have posted this page.

no moving parts. 

http://www.idatech.com/



Tom DeReggi wrote:
> Patrick,
>
> All excellent points, and reality checks. Thanks for the feedback!
>
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message - 
> From: "Patrick Shoemaker" 
> To: "WISPA General List" 
> Sent: Monday, August 03, 2009 5:58 PM
> Subject: Re: [WISPA] Small auto start generator
>
>
>   
>> I think you'll find that to get a propane/NG generator installed on a
>> commercial building rooftop, you'll be looking at $10k minimum using
>> even the cheapest Generac air-cooled units. You'll need a roofing
>> company to come out and modify the roof to provide a mounting surface
>> for the generator, that will probably be the biggest cost. Getting
>> management comfortable with modifying a $300k roof membrane could be an
>> issue as well. Then getting gas to the unit from the building's gas
>> supply will require a plumbing contractor, permits, inspections. Then
>> the electrical hookup- more permits and inspections and a licensed EC.
>>
>> I just got a quote for qty 8 110AH 12v AGM batteries for a new site:
>> $1500 including shipping.
>>
>> A note on the Generac air-cooled generators. They break. All generators
>> break. The key is routine testing and PM. The generac air-cooled models
>> don't have any provision for automatic alarm reporting. So when a
>> battery dies or gas valve sticks or spark plug fouls or whatever, you
>> won't know about it until a manual site inspection or the power goes
>> out. The better generators (and the Generac liquid cooled models) have
>> contact closures or RS232 interfaces to report these conditions to your
>> site monitoring system, in turn notifying you back at the NOC.
>>
>>
>> Patrick Shoemaker
>> Vector Data Systems LLC
>> shoemak...@vectordatasystems.com
>> office: (301) 358-1690 x36
>> http://www.vectordatasystems.com
>>
>>
>> Tom DeReggi wrote:
>> 
>>> We also use the triplite APS inverters with good quality Gel cell. 
>>> Actually,
>>> we got a good 15 years out of the existing C&D batteries, because we
>>> inherited them from Teligent days :-)
>>> But new, qty 4- 12V 150AH batteries in series for about 3500watt and 
>>> decent
>>> run-time is $1400. + $800 for replacement inverters.  (The Triplites 
>>> worked
>>> really well, but about half of them died by the end of eight years. We
>>> matched good inverters with good pre-existing batteries and vice versa.) 
>>> So
>>> our thought was Why not buy a $2000 generator for the run-time and 
>>> load,
>>> and then several smaller UPSes for infront to cover the surges, power
>>> conditioning, and monitoring? Ones that keep running even when batteries
>>> short out.  Part of the reason we are investigating is that we now have
>>> duplicate need of devices to power.  Some are AC devices like PC routers.
>>> Some are 20-24VDC w/AC adapters. Some are new licensed gear running on 
>>> 48V.
>>> Cost is increased having long battery run time on both seperate AC and DC
>>> backup power subsystems. And how do we plan for load growth? How many new
>>> radios installed will be AC or DC? Unlicensed versus Licensed? We really
>>> dont know in advance.  There is a lot of power waste going from AC to DC 
>>> to
>>> AC to DC.
>>>
>>> The thought was... If long run time was accomplished by the propaine
>>> generator, both DC and AC battery subsystems could be installed with 
>>> lower
>>> cost lower run-time batteries.  We'd still need to account for max watts
>>> growth for each subsystem, but we could way reduce AH requirements for 
>>> both
>>> subsystems.
>>>
>>> Or am I making this to complicated, and better just sticking with 
>>> batteries
>>> :-)
>>>
>>> Chris Erikson's idea on solar panels sounded interesting. Although, I bet 
>>> my
>>> ruthless roof rights people will try to charge me a monthly colo fee for
>>> them :-(
>>> I wonder if I can make the solar panels look like rain/weather shields 
>>> :-)
>>>
>>> Tom DeReggi
>>> RapidDSL & Wireless, Inc
>>> IntAirNet- Fixed Wireless Broadband
>>>
>>>
>>> - Original Message - 
>>> From: "jp" 
>>> To: "WI

Re: [WISPA] Small auto start generator

2009-08-04 Thread Chuck Profito
Let's not forget small nuclear power as sold in 1951! ... http://xrl.in/2u36


-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Curtis Maurand
Sent: Tuesday, August 04, 2009 10:39 AM
To: WISPA General List
Subject: Re: [WISPA] Small auto start generator


Fuel cells, too.

http://www.fuelcellmarkets.com/products_and_services/3,1,599,17,7561.html



Christopher Erickson wrote:
> The right type of batteries could give you 15 to 20 years of service.
>
> And adding a pair of solar panels and an MPPT solar charge controller
could
> increase your backup battery run time from a couple of days to a couple
> of weeks.  And no volatile fuel issues to deal with either.  And their PMI
> interval is a godsend too.  And cheaper than a genny.
>
> Add another panel or two and you might even be able to drop your grid
> connection.
>
> Remember to eliminate as many power conversions as possible from your
> telecom power design.
>
> -Christopher Erickson
> Network Design Engineer
> 5432 E. Northern Lights Blvd., Suite 529
> Anchorage, AK 99508
> N61?11.710' W149?46.723'
>
>
>   
>> -Original Message-
>> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]on
>> Behalf Of Tom DeReggi
>> Sent: Monday, August 03, 2009 10:49 AM
>> To: WISPA General List
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>> Patrick,
>>
>> In general, sounds like good advice.
>>
>> To clarify our intent, in posting.
>>
>> >From yr 2000-2008, our model was to
>>
>> 1) Have minimum 12 hour run-time of battery for core cell sites.
>> 2) Have contingency plan for hooking up a mobile gasoline powered
>> generator,
>> in longer lasting Emergencies.
>> (We have a couple hot spare generators)
>>
>> Why are we changing our view point?
>>
>> 1) Many of the batteries have now died, and need replaced. Batteries are
>> still very expensive. Propaine Generators have come way down in
>> price (aka
>> Generac) In most case, the generator will be less expensive than the
>> batteries, based on watt load at the sites.
>>
>> 2) Our network has grown, but our staff size has shrunk. We realize the
>> challenge that more than one site can loose power at once, and
>> harder to get
>> to multiple locations at once with generators.
>> Its hard to know when batteries will hold or not, when
>> towards the end
>> of their life, so its always a rush with the genrators. 9/10 cases by the
>> time we get generators onsite, the power gets restored within minutes.
>>
>> 3)  Its easy to throw a generator on a Grant Application :-)
>>
>> We believe permanent onsite generators would likely increase
>> uptime, and not
>> necessarilly be more expensive, for some of our sites. (We'd of
>> course still
>> keep some patteries inline) The question is whether it will be
>> more hassle
>> than we realize to re-fill them and inspect them. Some people told me
>> quarterly inspections are needed, or sometimes they do not start when
>> needed.
>>
>> We are already connected to building generators, where we were
>> allowed to,
>> so we are looking at sites where our only option was to put in our own.
>> I'm still uncertain what objections or preferences property
>> management would
>> have for this type stuff.  For example, whether they would be concerned
>> about it blowing up if a gas leak occured.
>>
>> I actually have one building in mind wher egetting a new electrical
>> connector from the roof to the ground would be really a big pain. Would
>> require Xray and drilling every floor of 20.
>> There I'd like to put a roof mounted propaine generator. I was thinking
>> maybe the best option is to just have a small external tank, and swap the
>> tank after use?
>>
>> I would think where there is pre-existing riser space, I'd want
>> to mount on
>> ground level, and run thick gauge AC wire up.
>>
>> Mostly I was wondering if management companies look for specific features
>> for the device, or if Generac would offer all standard features
>> to meet the
>> requirements of code and property managers.
>>
>> For our smaller watt sites, we'd of course stick with batteries.
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message -
>> From: "Patrick Shoemaker" 
>> To: "WISPA General List" 
>> Sent: Monda

Re: [WISPA] Small auto start generator

2009-08-04 Thread Curtis Maurand

Fuel cells, too.

http://www.fuelcellmarkets.com/products_and_services/3,1,599,17,7561.html



Christopher Erickson wrote:
> The right type of batteries could give you 15 to 20 years of service.
>
> And adding a pair of solar panels and an MPPT solar charge controller could
> increase your backup battery run time from a couple of days to a couple
> of weeks.  And no volatile fuel issues to deal with either.  And their PMI
> interval is a godsend too.  And cheaper than a genny.
>
> Add another panel or two and you might even be able to drop your grid
> connection.
>
> Remember to eliminate as many power conversions as possible from your
> telecom power design.
>
> -Christopher Erickson
> Network Design Engineer
> 5432 E. Northern Lights Blvd., Suite 529
> Anchorage, AK 99508
> N61?11.710' W149?46.723'
>
>
>   
>> -Original Message-
>> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]on
>> Behalf Of Tom DeReggi
>> Sent: Monday, August 03, 2009 10:49 AM
>> To: WISPA General List
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>> Patrick,
>>
>> In general, sounds like good advice.
>>
>> To clarify our intent, in posting.
>>
>> >From yr 2000-2008, our model was to
>>
>> 1) Have minimum 12 hour run-time of battery for core cell sites.
>> 2) Have contingency plan for hooking up a mobile gasoline powered
>> generator,
>> in longer lasting Emergencies.
>> (We have a couple hot spare generators)
>>
>> Why are we changing our view point?
>>
>> 1) Many of the batteries have now died, and need replaced. Batteries are
>> still very expensive. Propaine Generators have come way down in
>> price (aka
>> Generac) In most case, the generator will be less expensive than the
>> batteries, based on watt load at the sites.
>>
>> 2) Our network has grown, but our staff size has shrunk. We realize the
>> challenge that more than one site can loose power at once, and
>> harder to get
>> to multiple locations at once with generators.
>> Its hard to know when batteries will hold or not, when
>> towards the end
>> of their life, so its always a rush with the genrators. 9/10 cases by the
>> time we get generators onsite, the power gets restored within minutes.
>>
>> 3)  Its easy to throw a generator on a Grant Application :-)
>>
>> We believe permanent onsite generators would likely increase
>> uptime, and not
>> necessarilly be more expensive, for some of our sites. (We'd of
>> course still
>> keep some patteries inline) The question is whether it will be
>> more hassle
>> than we realize to re-fill them and inspect them. Some people told me
>> quarterly inspections are needed, or sometimes they do not start when
>> needed.
>>
>> We are already connected to building generators, where we were
>> allowed to,
>> so we are looking at sites where our only option was to put in our own.
>> I'm still uncertain what objections or preferences property
>> management would
>> have for this type stuff.  For example, whether they would be concerned
>> about it blowing up if a gas leak occured.
>>
>> I actually have one building in mind wher egetting a new electrical
>> connector from the roof to the ground would be really a big pain. Would
>> require Xray and drilling every floor of 20.
>> There I'd like to put a roof mounted propaine generator. I was thinking
>> maybe the best option is to just have a small external tank, and swap the
>> tank after use?
>>
>> I would think where there is pre-existing riser space, I'd want
>> to mount on
>> ground level, and run thick gauge AC wire up.
>>
>> Mostly I was wondering if management companies look for specific features
>> for the device, or if Generac would offer all standard features
>> to meet the
>> requirements of code and property managers.
>>
>> For our smaller watt sites, we'd of course stick with batteries.
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message -
>> From: "Patrick Shoemaker" 
>> To: "WISPA General List" 
>> Sent: Monday, August 03, 2009 9:07 AM
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>> 
>>> Yes, it's possible to get a generator installed on a roof, but it will
>>> be an expensive project in our area due to the code compliance issues.
>>> However, most comm

Re: [WISPA] Small auto start generator

2009-08-04 Thread Josh Luthman
Better yet exchange them to discount your new battery...

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

"When you have eliminated the impossible, that which remains, however
improbable, must be the truth."
--- Sir Arthur Conan Doyle


On Tue, Aug 4, 2009 at 11:16 AM, Marlon K. Schafer wrote:

> Old batteries are worth money.  The local napa will take them for free.
> marlon
>
>  - Original Message -
>  From: Brian Webster
>   To: WISPA General List
>  Sent: Monday, August 03, 2009 6:41 PM
>  Subject: Re: [WISPA] Small auto start generator
>
>
>   And don't forget the disposal costs of batteries when they are no longer
> functional. Telephone companies have an extensive HAZMAT documentation and
> chain of custody requirement for their switch batteries. Don't think this
> industry will get away with not having some requirement like that for long
> :-)
>
>
>
>  Thank You,
>  Brian Webster
>   
>
>
>
>  Tom DeReggi wrote:
> Patrick,
>
> In general, sounds like good advice.
>
> To clarify our intent, in posting.
>
> >From yr 2000-2008, our model was to
>
> 1) Have minimum 12 hour run-time of battery for core cell sites.
> 2) Have contingency plan for hooking up a mobile gasoline powered
> generator,
> in longer lasting Emergencies.
>(We have a couple hot spare generators)
>
> Why are we changing our view point?
>
> 1) Many of the batteries have now died, and need replaced. Batteries are
> still very expensive. Propaine Generators have come way down in price (aka
> Generac) In most case, the generator will be less expensive than the
> batteries, based on watt load at the sites.
>
> 2) Our network has grown, but our staff size has shrunk. We realize the
> challenge that more than one site can loose power at once, and harder to
> get
> to multiple locations at once with generators.
>Its hard to know when batteries will hold or not, when towards the end
> of their life, so its always a rush with the genrators. 9/10 cases by the
> time we get generators onsite, the power gets restored within minutes.
>
> 3)  Its easy to throw a generator on a Grant Application :-)
>
> We believe permanent onsite generators would likely increase uptime, and
> not
> necessarilly be more expensive, for some of our sites. (We'd of course
> still
> keep some patteries inline) The question is whether it will be more hassle
> than we realize to re-fill them and inspect them. Some people told me
> quarterly inspections are needed, or sometimes they do not start when
> needed.
>
> We are already connected to building generators, where we were allowed to,
> so we are looking at sites where our only option was to put in our own.
> I'm still uncertain what objections or preferences property management
> would
> have for this type stuff.  For example, whether they would be concerned
> about it blowing up if a gas leak occured.
>
> I actually have one building in mind wher egetting a new electrical
> connector from the roof to the ground would be really a big pain. Would
> require Xray and drilling every floor of 20.
> There I'd like to put a roof mounted propaine generator. I was thinking
> maybe the best option is to just have a small external tank, and swap the
> tank after use?
>
> I would think where there is pre-existing riser space, I'd want to mount on
> ground level, and run thick gauge AC wire up.
>
> Mostly I was wondering if management companies look for specific features
> for the device, or if Generac would offer all standard features to meet the
> requirements of code and property managers.
>
> For our smaller watt sites, we'd of course stick with batteries.
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message -
> From: "Patrick Shoemaker" 
> To: "WISPA General List" 
> Sent: Monday, August 03, 2009 9:07 AM
> Subject: Re: [WISPA] Small auto start generator
>
>
>  Yes, it's possible to get a generator installed on a roof, but it will
> be an expensive project in our area due to the code compliance issues.
> However, most commercial buildings will have a preexisting emergency
> power system for critical loads installed already. There are strict
> requirements such as sub 10 second startup times, routine testing, and
> fuel availability requirements. If you talk to the building engineer,
> you might be able to convince them to allow you a small amount of power
> from an emergency circuit. The buildings I am in do this for most of
> their tenants for phone systems, etc.
>
> Failing that, have an 

Re: [WISPA] Small auto start generator

2009-08-04 Thread Marlon K. Schafer
Old batteries are worth money.  The local napa will take them for free.
marlon

  - Original Message - 
  From: Brian Webster 
  To: WISPA General List 
  Sent: Monday, August 03, 2009 6:41 PM
  Subject: Re: [WISPA] Small auto start generator


  And don't forget the disposal costs of batteries when they are no longer 
functional. Telephone companies have an extensive HAZMAT documentation and 
chain of custody requirement for their switch batteries. Don't think this 
industry will get away with not having some requirement like that for long :-)



  Thank You,
  Brian Webster
  



  Tom DeReggi wrote: 
Patrick,

In general, sounds like good advice.

To clarify our intent, in posting.

>From yr 2000-2008, our model was to

1) Have minimum 12 hour run-time of battery for core cell sites.
2) Have contingency plan for hooking up a mobile gasoline powered generator, 
in longer lasting Emergencies.
(We have a couple hot spare generators)

Why are we changing our view point?

1) Many of the batteries have now died, and need replaced. Batteries are 
still very expensive. Propaine Generators have come way down in price (aka 
Generac) In most case, the generator will be less expensive than the 
batteries, based on watt load at the sites.

2) Our network has grown, but our staff size has shrunk. We realize the 
challenge that more than one site can loose power at once, and harder to get 
to multiple locations at once with generators.
Its hard to know when batteries will hold or not, when towards the end 
of their life, so its always a rush with the genrators. 9/10 cases by the 
time we get generators onsite, the power gets restored within minutes.

3)  Its easy to throw a generator on a Grant Application :-)

We believe permanent onsite generators would likely increase uptime, and not 
necessarilly be more expensive, for some of our sites. (We'd of course still 
keep some patteries inline) The question is whether it will be more hassle 
than we realize to re-fill them and inspect them. Some people told me 
quarterly inspections are needed, or sometimes they do not start when 
needed.

We are already connected to building generators, where we were allowed to, 
so we are looking at sites where our only option was to put in our own.
I'm still uncertain what objections or preferences property management would 
have for this type stuff.  For example, whether they would be concerned 
about it blowing up if a gas leak occured.

I actually have one building in mind wher egetting a new electrical 
connector from the roof to the ground would be really a big pain. Would 
require Xray and drilling every floor of 20.
There I'd like to put a roof mounted propaine generator. I was thinking 
maybe the best option is to just have a small external tank, and swap the 
tank after use?

I would think where there is pre-existing riser space, I'd want to mount on 
ground level, and run thick gauge AC wire up.

Mostly I was wondering if management companies look for specific features 
for the device, or if Generac would offer all standard features to meet the 
requirements of code and property managers.

For our smaller watt sites, we'd of course stick with batteries.

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Patrick Shoemaker" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 9:07 AM
Subject: Re: [WISPA] Small auto start generator


  Yes, it's possible to get a generator installed on a roof, but it will
be an expensive project in our area due to the code compliance issues.
However, most commercial buildings will have a preexisting emergency
power system for critical loads installed already. There are strict
requirements such as sub 10 second startup times, routine testing, and
fuel availability requirements. If you talk to the building engineer,
you might be able to convince them to allow you a small amount of power
from an emergency circuit. The buildings I am in do this for most of
their tenants for phone systems, etc.

Failing that, have an electrician run conduit to the parking lot and
place a power inlet down there. Be sure to have 24 hours of battery
capacity, and use a trailer-mounted generator in the parking lot for the
rare outage that lasts longer than the batteries.


Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


Tom DeReggi wrote:
While on the topic of generators.

Anyone have advice on how to accommodate generators in Commercial
Multi-tenant buildings.

Several things come to mind... Gas generators are definately not allowed 
on
roofs, for fire safety reasons.
Adequate ventilation is likely needed for either gas or Propain 
generators.

What type propain generators would likely gain permission to get 
installed
in a rooftop penthouse? or Roof?

If a propain

Re: [WISPA] Small auto start generator

2009-08-04 Thread Patrick Shoemaker
Here you go. I have been using these Universal Batteries for a few years 
now and have not had any problems so far.

http://www.factoriesonline.com/ProductInfo.aspx?id=1899684&categoryid=0

I have also purchased from that vendor before and not had a problem. 
Call them for a freight quote.

Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


jp wrote:
> On Mon, Aug 03, 2009 at 05:58:11PM -0400, Patrick Shoemaker wrote:
>> I just got a quote for qty 8 110AH 12v AGM batteries for a new site: 
>> $1500 including shipping.
>>
>> Patrick Shoemaker
>> Vector Data Systems LLC
>> shoemak...@vectordatasystems.com
>> office: (301) 358-1690 x36
>> http://www.vectordatasystems.com
>>
> 
> Mind sharing where to get AGM batts like that for that price?
> 



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-03 Thread jp
On Mon, Aug 03, 2009 at 05:58:11PM -0400, Patrick Shoemaker wrote:
> I think you'll find that to get a propane/NG generator installed on a 
> commercial building rooftop, you'll be looking at $10k minimum using 
> even the cheapest Generac air-cooled units. You'll need a roofing 
> company to come out and modify the roof to provide a mounting surface 
> for the generator, that will probably be the biggest cost. Getting 
> management comfortable with modifying a $300k roof membrane could be an 
> issue as well. Then getting gas to the unit from the building's gas 
> supply will require a plumbing contractor, permits, inspections. Then 
> the electrical hookup- more permits and inspections and a licensed EC.

Also add a $1-3k for a good auto transfer switch.

Maintenance such as oil changes and testing can also run a couple 
hundred a year in labor and materials, so that adds up over the life of 
the backup power solution. 

We've also seen propane delivery companies forget to keep the tanks full 
due to the unpredictable propane usage. And we've had weather so bad, 
propane trucks couldn't refill till spring if they wanted to.

I am a big fan of whole building generators though. It's warm and fuzzy 
to keep a building going like normal when nobody else has power.

I certainly understand the need for planning power consumption to scale 
with needs and growth. We consider power consumption in almost every 
equipment purchase or upgrade. Many upgrades decrease power consumption, 
like newer managed switches or newer PC hardware, making site runtime 
better.

> I just got a quote for qty 8 110AH 12v AGM batteries for a new site: 
> $1500 including shipping.
> 
> A note on the Generac air-cooled generators. They break. All generators 
> break. The key is routine testing and PM. The generac air-cooled models 
> don't have any provision for automatic alarm reporting. So when a 
> battery dies or gas valve sticks or spark plug fouls or whatever, you 
> won't know about it until a manual site inspection or the power goes 
> out. The better generators (and the Generac liquid cooled models) have 
> contact closures or RS232 interfaces to report these conditions to your 
> site monitoring system, in turn notifying you back at the NOC.
> 
> 
> Patrick Shoemaker
> Vector Data Systems LLC
> shoemak...@vectordatasystems.com
> office: (301) 358-1690 x36
> http://www.vectordatasystems.com
> 
> 
> Tom DeReggi wrote:
> > We also use the triplite APS inverters with good quality Gel cell. 
> > Actually, 
> > we got a good 15 years out of the existing C&D batteries, because we 
> > inherited them from Teligent days :-)
> > But new, qty 4- 12V 150AH batteries in series for about 3500watt and decent 
> > run-time is $1400. + $800 for replacement inverters.  (The Triplites worked 
> > really well, but about half of them died by the end of eight years. We 
> > matched good inverters with good pre-existing batteries and vice versa.)  
> > So 
> > our thought was Why not buy a $2000 generator for the run-time and 
> > load, 
> > and then several smaller UPSes for infront to cover the surges, power 
> > conditioning, and monitoring? Ones that keep running even when batteries 
> > short out.  Part of the reason we are investigating is that we now have 
> > duplicate need of devices to power.  Some are AC devices like PC routers. 
> > Some are 20-24VDC w/AC adapters. Some are new licensed gear running on 48V. 
> > Cost is increased having long battery run time on both seperate AC and DC 
> > backup power subsystems. And how do we plan for load growth? How many new 
> > radios installed will be AC or DC? Unlicensed versus Licensed? We really 
> > dont know in advance.  There is a lot of power waste going from AC to DC to 
> > AC to DC.
> > 
> > The thought was... If long run time was accomplished by the propaine 
> > generator, both DC and AC battery subsystems could be installed with lower 
> > cost lower run-time batteries.  We'd still need to account for max watts 
> > growth for each subsystem, but we could way reduce AH requirements for both 
> > subsystems.
> > 
> > Or am I making this to complicated, and better just sticking with batteries 
> > :-)
> > 
> > Chris Erikson's idea on solar panels sounded interesting. Although, I bet 
> > my 
> > ruthless roof rights people will try to charge me a monthly colo fee for 
> > them :-(
> > I wonder if I can make the solar panels look like rain/weather shields :-)
> > 
> > Tom DeReggi
> > RapidDSL & Wireless, Inc
> > IntAirNet- Fixed Wireless Broadband
> > 
> > 
> > - Origi

Re: [WISPA] Small auto start generator

2009-08-03 Thread jp
On Mon, Aug 03, 2009 at 05:58:11PM -0400, Patrick Shoemaker wrote:
> 
> I just got a quote for qty 8 110AH 12v AGM batteries for a new site: 
> $1500 including shipping.
> 
> Patrick Shoemaker
> Vector Data Systems LLC
> shoemak...@vectordatasystems.com
> office: (301) 358-1690 x36
> http://www.vectordatasystems.com
> 

Mind sharing where to get AGM batts like that for that price?

-- 
/*
Jason Philbrook   |   Midcoast Internet Solutions - Wireless and DSL
KB1IOJ|   Broadband Internet Access, Dialup, and Hosting 
 http://f64.nu/   |   for Midcoast Mainehttp://www.midcoast.com/
*/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-03 Thread Blake Bowers
Its really not onerous requirements.   Basically you need
to dispose of them with a true battery recylcer - often times
the scrap dealer down the road.

As long as they provide documenation that you took them to
someone reputable in the chain, you are fine.

A typical flooded CO battery weighs in at around 400 lbs, the
last ones we removed got .15 cents a lb, with paper trail to Doe
Run MO.

The site had over 48 of them.

You need a special sling to move them...  If anyone has to
I can give details.


Don't take your organs to heaven,
heaven knows we need them down here!
Be an organ donor, sign your donor card today.

- Original Message - 
From: "Brian Webster" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 8:41 PM
Subject: Re: [WISPA] Small auto start generator


> And don't forget the disposal costs of batteries when they are no longer 
> functional. Telephone companies have an extensive HAZMAT documentation and 
> chain of custody requirement for their switch batteries. Don't think this 
> industry will get away with not having some requirement like that for long 
> :-)
>
>
>
> Thank You,
> Brian Webster
> 
>
>
>
> Tom DeReggi wrote:
> Patrick,
>
> In general, sounds like good advice.
>
> To clarify our intent, in posting.
>
>>From yr 2000-2008, our model was to
>
> 1) Have minimum 12 hour run-time of battery for core cell sites.
> 2) Have contingency plan for hooking up a mobile gasoline powered 
> generator,
> in longer lasting Emergencies.
>(We have a couple hot spare generators)
>
> Why are we changing our view point?
>
> 1) Many of the batteries have now died, and need replaced. Batteries are
> still very expensive. Propaine Generators have come way down in price (aka
> Generac) In most case, the generator will be less expensive than the
> batteries, based on watt load at the sites.
>
> 2) Our network has grown, but our staff size has shrunk. We realize the
> challenge that more than one site can loose power at once, and harder to 
> get
> to multiple locations at once with generators.
>Its hard to know when batteries will hold or not, when towards the end
> of their life, so its always a rush with the genrators. 9/10 cases by the
> time we get generators onsite, the power gets restored within minutes.
>
> 3)  Its easy to throw a generator on a Grant Application :-)
>
> We believe permanent onsite generators would likely increase uptime, and 
> not
> necessarilly be more expensive, for some of our sites. (We'd of course 
> still
> keep some patteries inline) The question is whether it will be more hassle
> than we realize to re-fill them and inspect them. Some people told me
> quarterly inspections are needed, or sometimes they do not start when
> needed.
>
> We are already connected to building generators, where we were allowed to,
> so we are looking at sites where our only option was to put in our own.
> I'm still uncertain what objections or preferences property management 
> would
> have for this type stuff.  For example, whether they would be concerned
> about it blowing up if a gas leak occured.
>
> I actually have one building in mind wher egetting a new electrical
> connector from the roof to the ground would be really a big pain. Would
> require Xray and drilling every floor of 20.
> There I'd like to put a roof mounted propaine generator. I was thinking
> maybe the best option is to just have a small external tank, and swap the
> tank after use?
>
> I would think where there is pre-existing riser space, I'd want to mount 
> on
> ground level, and run thick gauge AC wire up.
>
> Mostly I was wondering if management companies look for specific features
> for the device, or if Generac would offer all standard features to meet 
> the
> requirements of code and property managers.
>
> For our smaller watt sites, we'd of course stick with batteries.
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message - 
> From: "Patrick Shoemaker" 
> To: "WISPA General List" 
> Sent: Monday, August 03, 2009 9:07 AM
> Subject: Re: [WISPA] Small auto start generator
>
>
>  Yes, it's possible to get a generator installed on a roof, but it will
> be an expensive project in our area due to the code compliance issues.
> However, most commercial buildings will have a preexisting emergency
> power system for critical loads installed already. There are strict
> requirements such as sub 10 second startup times, routine testing, and
> fuel availability requirements. If you talk to the building engineer,
> you might be able to convince them t

Re: [WISPA] Small auto start generator

2009-08-03 Thread Brian Webster




And don't forget the disposal costs of batteries
when they are no longer functional. Telephone companies have an
extensive HAZMAT documentation and chain of custody requirement for
their switch batteries. Don't think this industry will get away with
not having some requirement like that for long :-)









Thank You,



Thank You,
Brian Webster





Tom DeReggi wrote:

  Patrick,

In general, sounds like good advice.

To clarify our intent, in posting.

>From yr 2000-2008, our model was to

1) Have minimum 12 hour run-time of battery for core cell sites.
2) Have contingency plan for hooking up a mobile gasoline powered generator, 
in longer lasting Emergencies.
(We have a couple hot spare generators)

Why are we changing our view point?

1) Many of the batteries have now died, and need replaced. Batteries are 
still very expensive. Propaine Generators have come way down in price (aka 
Generac) In most case, the generator will be less expensive than the 
batteries, based on watt load at the sites.

2) Our network has grown, but our staff size has shrunk. We realize the 
challenge that more than one site can loose power at once, and harder to get 
to multiple locations at once with generators.
Its hard to know when batteries will hold or not, when towards the end 
of their life, so its always a rush with the genrators. 9/10 cases by the 
time we get generators onsite, the power gets restored within minutes.

3)  Its easy to throw a generator on a Grant Application :-)

We believe permanent onsite generators would likely increase uptime, and not 
necessarilly be more expensive, for some of our sites. (We'd of course still 
keep some patteries inline) The question is whether it will be more hassle 
than we realize to re-fill them and inspect them. Some people told me 
quarterly inspections are needed, or sometimes they do not start when 
needed.

We are already connected to building generators, where we were allowed to, 
so we are looking at sites where our only option was to put in our own.
I'm still uncertain what objections or preferences property management would 
have for this type stuff.  For example, whether they would be concerned 
about it blowing up if a gas leak occured.

I actually have one building in mind wher egetting a new electrical 
connector from the roof to the ground would be really a big pain. Would 
require Xray and drilling every floor of 20.
There I'd like to put a roof mounted propaine generator. I was thinking 
maybe the best option is to just have a small external tank, and swap the 
tank after use?

I would think where there is pre-existing riser space, I'd want to mount on 
ground level, and run thick gauge AC wire up.

Mostly I was wondering if management companies look for specific features 
for the device, or if Generac would offer all standard features to meet the 
requirements of code and property managers.

For our smaller watt sites, we'd of course stick with batteries.

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Patrick Shoemaker" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 9:07 AM
Subject: Re: [WISPA] Small auto start generator


  
  
Yes, it's possible to get a generator installed on a roof, but it will
be an expensive project in our area due to the code compliance issues.
However, most commercial buildings will have a preexisting emergency
power system for critical loads installed already. There are strict
requirements such as sub 10 second startup times, routine testing, and
fuel availability requirements. If you talk to the building engineer,
you might be able to convince them to allow you a small amount of power
from an emergency circuit. The buildings I am in do this for most of
their tenants for phone systems, etc.

Failing that, have an electrician run conduit to the parking lot and
place a power inlet down there. Be sure to have 24 hours of battery
capacity, and use a trailer-mounted generator in the parking lot for the
rare outage that lasts longer than the batteries.


Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


Tom DeReggi wrote:


  While on the topic of generators.

Anyone have advice on how to accommodate generators in Commercial
Multi-tenant buildings.

Several things come to mind... Gas generators are definately not allowed 
on
roofs, for fire safety reasons.
Adequate ventilation is likely needed for either gas or Propain 
generators.

What type propain generators would likely gain permission to get 
installed
in a rooftop penthouse? or Roof?

If a propain generator was used on a top floor, how would Propain get
re-fueled easilly?
Is is standard proceedure to have removable tanks, and just have new 
tanks
swapped (like a gas grill).?
Or is is customary to have tanks on

Re: [WISPA] Small auto start generator

2009-08-03 Thread Tom DeReggi
Patrick,

All excellent points, and reality checks. Thanks for the feedback!


Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Patrick Shoemaker" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 5:58 PM
Subject: Re: [WISPA] Small auto start generator


>I think you'll find that to get a propane/NG generator installed on a
> commercial building rooftop, you'll be looking at $10k minimum using
> even the cheapest Generac air-cooled units. You'll need a roofing
> company to come out and modify the roof to provide a mounting surface
> for the generator, that will probably be the biggest cost. Getting
> management comfortable with modifying a $300k roof membrane could be an
> issue as well. Then getting gas to the unit from the building's gas
> supply will require a plumbing contractor, permits, inspections. Then
> the electrical hookup- more permits and inspections and a licensed EC.
>
> I just got a quote for qty 8 110AH 12v AGM batteries for a new site:
> $1500 including shipping.
>
> A note on the Generac air-cooled generators. They break. All generators
> break. The key is routine testing and PM. The generac air-cooled models
> don't have any provision for automatic alarm reporting. So when a
> battery dies or gas valve sticks or spark plug fouls or whatever, you
> won't know about it until a manual site inspection or the power goes
> out. The better generators (and the Generac liquid cooled models) have
> contact closures or RS232 interfaces to report these conditions to your
> site monitoring system, in turn notifying you back at the NOC.
>
>
> Patrick Shoemaker
> Vector Data Systems LLC
> shoemak...@vectordatasystems.com
> office: (301) 358-1690 x36
> http://www.vectordatasystems.com
>
>
> Tom DeReggi wrote:
>> We also use the triplite APS inverters with good quality Gel cell. 
>> Actually,
>> we got a good 15 years out of the existing C&D batteries, because we
>> inherited them from Teligent days :-)
>> But new, qty 4- 12V 150AH batteries in series for about 3500watt and 
>> decent
>> run-time is $1400. + $800 for replacement inverters.  (The Triplites 
>> worked
>> really well, but about half of them died by the end of eight years. We
>> matched good inverters with good pre-existing batteries and vice versa.) 
>> So
>> our thought was Why not buy a $2000 generator for the run-time and 
>> load,
>> and then several smaller UPSes for infront to cover the surges, power
>> conditioning, and monitoring? Ones that keep running even when batteries
>> short out.  Part of the reason we are investigating is that we now have
>> duplicate need of devices to power.  Some are AC devices like PC routers.
>> Some are 20-24VDC w/AC adapters. Some are new licensed gear running on 
>> 48V.
>> Cost is increased having long battery run time on both seperate AC and DC
>> backup power subsystems. And how do we plan for load growth? How many new
>> radios installed will be AC or DC? Unlicensed versus Licensed? We really
>> dont know in advance.  There is a lot of power waste going from AC to DC 
>> to
>> AC to DC.
>>
>> The thought was... If long run time was accomplished by the propaine
>> generator, both DC and AC battery subsystems could be installed with 
>> lower
>> cost lower run-time batteries.  We'd still need to account for max watts
>> growth for each subsystem, but we could way reduce AH requirements for 
>> both
>> subsystems.
>>
>> Or am I making this to complicated, and better just sticking with 
>> batteries
>> :-)
>>
>> Chris Erikson's idea on solar panels sounded interesting. Although, I bet 
>> my
>> ruthless roof rights people will try to charge me a monthly colo fee for
>> them :-(
>> I wonder if I can make the solar panels look like rain/weather shields 
>> :-)
>>
>> Tom DeReggi
>> RapidDSL & Wireless, Inc
>> IntAirNet- Fixed Wireless Broadband
>>
>>
>> - Original Message - 
>> From: "jp" 
>> To: "WISPA General List" 
>> Sent: Monday, August 03, 2009 12:11 PM
>> Subject: Re: [WISPA] Small auto start generator
>>
>>
>>> The tripplite APS is what we use for this. Small generators are a pain.
>>>
>>> On Sun, Aug 02, 2009 at 02:57:23PM -0430, os10ru...@gmail.com wrote:
>>>> You might want something like an inverter (Xantrex for example) which
>>>> includes a DC to AC inverter, battery charger, and automatic transfer
>>>> switch. Add the batteries

Re: [WISPA] Small auto start generator

2009-08-03 Thread Brian Rohrbacher




Put the word GREEN in that grant app and you might just have a shot! 
Not too bad of an idea with those solar panels.

Brian

Christopher Erickson wrote:

  The right type of batteries could give you 15 to 20 years of service.

And adding a pair of solar panels and an MPPT solar charge controller could
increase your backup battery run time from a couple of days to a couple
of weeks.  And no volatile fuel issues to deal with either.  And their PMI
interval is a godsend too.  And cheaper than a genny.

Add another panel or two and you might even be able to drop your grid
connection.

Remember to eliminate as many power conversions as possible from your
telecom power design.

-Christopher Erickson
Network Design Engineer
5432 E. Northern Lights Blvd., Suite 529
Anchorage, AK 99508
N61?11.710' W149?46.723'


  
  
-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]On
Behalf Of Tom DeReggi
Sent: Monday, August 03, 2009 10:49 AM
To: WISPA General List
Subject: Re: [WISPA] Small auto start generator


Patrick,

In general, sounds like good advice.

To clarify our intent, in posting.

>From yr 2000-2008, our model was to

1) Have minimum 12 hour run-time of battery for core cell sites.
2) Have contingency plan for hooking up a mobile gasoline powered
generator,
in longer lasting Emergencies.
(We have a couple hot spare generators)

Why are we changing our view point?

1) Many of the batteries have now died, and need replaced. Batteries are
still very expensive. Propaine Generators have come way down in
price (aka
Generac) In most case, the generator will be less expensive than the
batteries, based on watt load at the sites.

2) Our network has grown, but our staff size has shrunk. We realize the
challenge that more than one site can loose power at once, and
harder to get
to multiple locations at once with generators.
Its hard to know when batteries will hold or not, when
towards the end
of their life, so its always a rush with the genrators. 9/10 cases by the
time we get generators onsite, the power gets restored within minutes.

3)  Its easy to throw a generator on a Grant Application :-)

We believe permanent onsite generators would likely increase
uptime, and not
necessarilly be more expensive, for some of our sites. (We'd of
course still
keep some patteries inline) The question is whether it will be
more hassle
than we realize to re-fill them and inspect them. Some people told me
quarterly inspections are needed, or sometimes they do not start when
needed.

We are already connected to building generators, where we were
allowed to,
so we are looking at sites where our only option was to put in our own.
I'm still uncertain what objections or preferences property
management would
have for this type stuff.  For example, whether they would be concerned
about it blowing up if a gas leak occured.

I actually have one building in mind wher egetting a new electrical
connector from the roof to the ground would be really a big pain. Would
require Xray and drilling every floor of 20.
There I'd like to put a roof mounted propaine generator. I was thinking
maybe the best option is to just have a small external tank, and swap the
tank after use?

I would think where there is pre-existing riser space, I'd want
to mount on
ground level, and run thick gauge AC wire up.

Mostly I was wondering if management companies look for specific features
for the device, or if Generac would offer all standard features
to meet the
requirements of code and property managers.

For our smaller watt sites, we'd of course stick with batteries.

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message -
From: "Patrick Shoemaker" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 9:07 AM
Subject: Re: [WISPA] Small auto start generator




  Yes, it's possible to get a generator installed on a roof, but it will
be an expensive project in our area due to the code compliance issues.
However, most commercial buildings will have a preexisting emergency
power system for critical loads installed already. There are strict
requirements such as sub 10 second startup times, routine testing, and
fuel availability requirements. If you talk to the building engineer,
you might be able to convince them to allow you a small amount of power
from an emergency circuit. The buildings I am in do this for most of
their tenants for phone systems, etc.

Failing that, have an electrician run conduit to the parking lot and
place a power inlet down there. Be sure to have 24 hours of battery
capacity, and use a trailer-mounted generator in the parking lot for the
rare outage that lasts longer than the batteries.


Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


Tom DeReggi wrote:
  
 

Re: [WISPA] Small auto start generator

2009-08-03 Thread Patrick Shoemaker
I think you'll find that to get a propane/NG generator installed on a 
commercial building rooftop, you'll be looking at $10k minimum using 
even the cheapest Generac air-cooled units. You'll need a roofing 
company to come out and modify the roof to provide a mounting surface 
for the generator, that will probably be the biggest cost. Getting 
management comfortable with modifying a $300k roof membrane could be an 
issue as well. Then getting gas to the unit from the building's gas 
supply will require a plumbing contractor, permits, inspections. Then 
the electrical hookup- more permits and inspections and a licensed EC.

I just got a quote for qty 8 110AH 12v AGM batteries for a new site: 
$1500 including shipping.

A note on the Generac air-cooled generators. They break. All generators 
break. The key is routine testing and PM. The generac air-cooled models 
don't have any provision for automatic alarm reporting. So when a 
battery dies or gas valve sticks or spark plug fouls or whatever, you 
won't know about it until a manual site inspection or the power goes 
out. The better generators (and the Generac liquid cooled models) have 
contact closures or RS232 interfaces to report these conditions to your 
site monitoring system, in turn notifying you back at the NOC.


Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


Tom DeReggi wrote:
> We also use the triplite APS inverters with good quality Gel cell. Actually, 
> we got a good 15 years out of the existing C&D batteries, because we 
> inherited them from Teligent days :-)
> But new, qty 4- 12V 150AH batteries in series for about 3500watt and decent 
> run-time is $1400. + $800 for replacement inverters.  (The Triplites worked 
> really well, but about half of them died by the end of eight years. We 
> matched good inverters with good pre-existing batteries and vice versa.)  So 
> our thought was Why not buy a $2000 generator for the run-time and load, 
> and then several smaller UPSes for infront to cover the surges, power 
> conditioning, and monitoring? Ones that keep running even when batteries 
> short out.  Part of the reason we are investigating is that we now have 
> duplicate need of devices to power.  Some are AC devices like PC routers. 
> Some are 20-24VDC w/AC adapters. Some are new licensed gear running on 48V. 
> Cost is increased having long battery run time on both seperate AC and DC 
> backup power subsystems. And how do we plan for load growth? How many new 
> radios installed will be AC or DC? Unlicensed versus Licensed? We really 
> dont know in advance.  There is a lot of power waste going from AC to DC to 
> AC to DC.
> 
> The thought was... If long run time was accomplished by the propaine 
> generator, both DC and AC battery subsystems could be installed with lower 
> cost lower run-time batteries.  We'd still need to account for max watts 
> growth for each subsystem, but we could way reduce AH requirements for both 
> subsystems.
> 
> Or am I making this to complicated, and better just sticking with batteries 
> :-)
> 
> Chris Erikson's idea on solar panels sounded interesting. Although, I bet my 
> ruthless roof rights people will try to charge me a monthly colo fee for 
> them :-(
> I wonder if I can make the solar panels look like rain/weather shields :-)
> 
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
> 
> 
> - Original Message - 
> From: "jp" 
> To: "WISPA General List" 
> Sent: Monday, August 03, 2009 12:11 PM
> Subject: Re: [WISPA] Small auto start generator
> 
> 
>> The tripplite APS is what we use for this. Small generators are a pain.
>>
>> On Sun, Aug 02, 2009 at 02:57:23PM -0430, os10ru...@gmail.com wrote:
>>> You might want something like an inverter (Xantrex for example) which
>>> includes a DC to AC inverter, battery charger, and automatic transfer
>>> switch. Add the batteries and you're done.
>>>
>>> Greg
>>>
>>> On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:
>>>
>>>> Thank you,
>>>> That is very good advice. After some research, I'm leaning toward a
>>>> UPS.
>>>>
>>>> A pair of good AGM batteries and charge controller will cost less
>>>> and be far less maintainence. Then I'd just run the CMM off the
>>>> batteries @ 24VDC.
>>>>
>>>> Thanks again
>>>> Jerry
>>>>
>>>>
>>>> -Original Message-
>>>> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]
>>>> On Behalf Of 

Re: [WISPA] Small auto start generator

2009-08-03 Thread Tom DeReggi
We also use the triplite APS inverters with good quality Gel cell. Actually, 
we got a good 15 years out of the existing C&D batteries, because we 
inherited them from Teligent days :-)
But new, qty 4- 12V 150AH batteries in series for about 3500watt and decent 
run-time is $1400. + $800 for replacement inverters.  (The Triplites worked 
really well, but about half of them died by the end of eight years. We 
matched good inverters with good pre-existing batteries and vice versa.)  So 
our thought was Why not buy a $2000 generator for the run-time and load, 
and then several smaller UPSes for infront to cover the surges, power 
conditioning, and monitoring? Ones that keep running even when batteries 
short out.  Part of the reason we are investigating is that we now have 
duplicate need of devices to power.  Some are AC devices like PC routers. 
Some are 20-24VDC w/AC adapters. Some are new licensed gear running on 48V. 
Cost is increased having long battery run time on both seperate AC and DC 
backup power subsystems. And how do we plan for load growth? How many new 
radios installed will be AC or DC? Unlicensed versus Licensed? We really 
dont know in advance.  There is a lot of power waste going from AC to DC to 
AC to DC.

The thought was... If long run time was accomplished by the propaine 
generator, both DC and AC battery subsystems could be installed with lower 
cost lower run-time batteries.  We'd still need to account for max watts 
growth for each subsystem, but we could way reduce AH requirements for both 
subsystems.

Or am I making this to complicated, and better just sticking with batteries 
:-)

Chris Erikson's idea on solar panels sounded interesting. Although, I bet my 
ruthless roof rights people will try to charge me a monthly colo fee for 
them :-(
I wonder if I can make the solar panels look like rain/weather shields :-)

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "jp" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 12:11 PM
Subject: Re: [WISPA] Small auto start generator


> The tripplite APS is what we use for this. Small generators are a pain.
>
> On Sun, Aug 02, 2009 at 02:57:23PM -0430, os10ru...@gmail.com wrote:
>> You might want something like an inverter (Xantrex for example) which
>> includes a DC to AC inverter, battery charger, and automatic transfer
>> switch. Add the batteries and you're done.
>>
>> Greg
>>
>> On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:
>>
>> > Thank you,
>> > That is very good advice. After some research, I'm leaning toward a
>> > UPS.
>> >
>> > A pair of good AGM batteries and charge controller will cost less
>> > and be far less maintainence. Then I'd just run the CMM off the
>> > batteries @ 24VDC.
>> >
>> > Thanks again
>> > Jerry
>> >
>> >
>> > -----Original Message-
>> > From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]
>> > On Behalf Of Gary Garrett
>> > Sent: Sunday, August 02, 2009 11:59 AM
>> > To: WISPA General List
>> > Subject: Re: [WISPA] Small auto start generator
>> >
>> > Small generators do not auto start very reliably.
>> > When cold or dampness causes hard starting the starter can overheat
>> > and
>> > burn out. Generally you need an electric choke to start gas engines,
>> > propane can "flood" and need to rest before trying again, diesel can
>> > be
>> > REAL hard to start when cold. Auto starters can not adapt to changing
>> > conditions.
>> > Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase.
>> > (1955
>> > Model)
>> > The monitor cranks for 1 min then rests and tries 3 times.
>> > Everything is
>> > adjustable. It knows to stop cranking when it sees AC voltage from the
>> > Gen. so the motor over runs the starter for just a few seconds. Only a
>> > huge starter motor can take this abuse and last unattended.
>> >
>> > You may be money ahead to find out why the existing generator is not
>> > starting and get it fixed.
>> >
>> > Jerry Richardson wrote:
>> >> We rent on a tower that is suspposed to have gen-set backup but it
>> >> does not start reliably.
>> >>
>> >> Any recommendations on a small auto-start generator? We only need
>> >> to power a CMMmicro - ~100watts.
>> >>
>> >> Thanks
>> >>
>> >>
>> >>
>> >> __
>> >> Jerry Richardson
>> >> airC

Re: [WISPA] Small auto start generator

2009-08-03 Thread Christopher Erickson
The right type of batteries could give you 15 to 20 years of service.

And adding a pair of solar panels and an MPPT solar charge controller could
increase your backup battery run time from a couple of days to a couple
of weeks.  And no volatile fuel issues to deal with either.  And their PMI
interval is a godsend too.  And cheaper than a genny.

Add another panel or two and you might even be able to drop your grid
connection.

Remember to eliminate as many power conversions as possible from your
telecom power design.

-Christopher Erickson
Network Design Engineer
5432 E. Northern Lights Blvd., Suite 529
Anchorage, AK 99508
N61?11.710' W149?46.723'


> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]on
> Behalf Of Tom DeReggi
> Sent: Monday, August 03, 2009 10:49 AM
> To: WISPA General List
> Subject: Re: [WISPA] Small auto start generator
>
>
> Patrick,
>
> In general, sounds like good advice.
>
> To clarify our intent, in posting.
>
> >From yr 2000-2008, our model was to
>
> 1) Have minimum 12 hour run-time of battery for core cell sites.
> 2) Have contingency plan for hooking up a mobile gasoline powered
> generator,
> in longer lasting Emergencies.
> (We have a couple hot spare generators)
>
> Why are we changing our view point?
>
> 1) Many of the batteries have now died, and need replaced. Batteries are
> still very expensive. Propaine Generators have come way down in
> price (aka
> Generac) In most case, the generator will be less expensive than the
> batteries, based on watt load at the sites.
>
> 2) Our network has grown, but our staff size has shrunk. We realize the
> challenge that more than one site can loose power at once, and
> harder to get
> to multiple locations at once with generators.
> Its hard to know when batteries will hold or not, when
> towards the end
> of their life, so its always a rush with the genrators. 9/10 cases by the
> time we get generators onsite, the power gets restored within minutes.
>
> 3)  Its easy to throw a generator on a Grant Application :-)
>
> We believe permanent onsite generators would likely increase
> uptime, and not
> necessarilly be more expensive, for some of our sites. (We'd of
> course still
> keep some patteries inline) The question is whether it will be
> more hassle
> than we realize to re-fill them and inspect them. Some people told me
> quarterly inspections are needed, or sometimes they do not start when
> needed.
>
> We are already connected to building generators, where we were
> allowed to,
> so we are looking at sites where our only option was to put in our own.
> I'm still uncertain what objections or preferences property
> management would
> have for this type stuff.  For example, whether they would be concerned
> about it blowing up if a gas leak occured.
>
> I actually have one building in mind wher egetting a new electrical
> connector from the roof to the ground would be really a big pain. Would
> require Xray and drilling every floor of 20.
> There I'd like to put a roof mounted propaine generator. I was thinking
> maybe the best option is to just have a small external tank, and swap the
> tank after use?
>
> I would think where there is pre-existing riser space, I'd want
> to mount on
> ground level, and run thick gauge AC wire up.
>
> Mostly I was wondering if management companies look for specific features
> for the device, or if Generac would offer all standard features
> to meet the
> requirements of code and property managers.
>
> For our smaller watt sites, we'd of course stick with batteries.
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> - Original Message -
> From: "Patrick Shoemaker" 
> To: "WISPA General List" 
> Sent: Monday, August 03, 2009 9:07 AM
> Subject: Re: [WISPA] Small auto start generator
>
>
> > Yes, it's possible to get a generator installed on a roof, but it will
> > be an expensive project in our area due to the code compliance issues.
> > However, most commercial buildings will have a preexisting emergency
> > power system for critical loads installed already. There are strict
> > requirements such as sub 10 second startup times, routine testing, and
> > fuel availability requirements. If you talk to the building engineer,
> > you might be able to convince them to allow you a small amount of power
> > from an emergency circuit. The buildings I am in do this for most of
> > their tenants for phone systems, etc.
> >
> > Failing that, have an electrician run conduit to the parking lot and
> > plac

Re: [WISPA] Small auto start generator

2009-08-03 Thread Tom DeReggi
Patrick,

In general, sounds like good advice.

To clarify our intent, in posting.

>From yr 2000-2008, our model was to

1) Have minimum 12 hour run-time of battery for core cell sites.
2) Have contingency plan for hooking up a mobile gasoline powered generator, 
in longer lasting Emergencies.
(We have a couple hot spare generators)

Why are we changing our view point?

1) Many of the batteries have now died, and need replaced. Batteries are 
still very expensive. Propaine Generators have come way down in price (aka 
Generac) In most case, the generator will be less expensive than the 
batteries, based on watt load at the sites.

2) Our network has grown, but our staff size has shrunk. We realize the 
challenge that more than one site can loose power at once, and harder to get 
to multiple locations at once with generators.
Its hard to know when batteries will hold or not, when towards the end 
of their life, so its always a rush with the genrators. 9/10 cases by the 
time we get generators onsite, the power gets restored within minutes.

3)  Its easy to throw a generator on a Grant Application :-)

We believe permanent onsite generators would likely increase uptime, and not 
necessarilly be more expensive, for some of our sites. (We'd of course still 
keep some patteries inline) The question is whether it will be more hassle 
than we realize to re-fill them and inspect them. Some people told me 
quarterly inspections are needed, or sometimes they do not start when 
needed.

We are already connected to building generators, where we were allowed to, 
so we are looking at sites where our only option was to put in our own.
I'm still uncertain what objections or preferences property management would 
have for this type stuff.  For example, whether they would be concerned 
about it blowing up if a gas leak occured.

I actually have one building in mind wher egetting a new electrical 
connector from the roof to the ground would be really a big pain. Would 
require Xray and drilling every floor of 20.
There I'd like to put a roof mounted propaine generator. I was thinking 
maybe the best option is to just have a small external tank, and swap the 
tank after use?

I would think where there is pre-existing riser space, I'd want to mount on 
ground level, and run thick gauge AC wire up.

Mostly I was wondering if management companies look for specific features 
for the device, or if Generac would offer all standard features to meet the 
requirements of code and property managers.

For our smaller watt sites, we'd of course stick with batteries.

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Patrick Shoemaker" 
To: "WISPA General List" 
Sent: Monday, August 03, 2009 9:07 AM
Subject: Re: [WISPA] Small auto start generator


> Yes, it's possible to get a generator installed on a roof, but it will
> be an expensive project in our area due to the code compliance issues.
> However, most commercial buildings will have a preexisting emergency
> power system for critical loads installed already. There are strict
> requirements such as sub 10 second startup times, routine testing, and
> fuel availability requirements. If you talk to the building engineer,
> you might be able to convince them to allow you a small amount of power
> from an emergency circuit. The buildings I am in do this for most of
> their tenants for phone systems, etc.
>
> Failing that, have an electrician run conduit to the parking lot and
> place a power inlet down there. Be sure to have 24 hours of battery
> capacity, and use a trailer-mounted generator in the parking lot for the
> rare outage that lasts longer than the batteries.
>
>
> Patrick Shoemaker
> Vector Data Systems LLC
> shoemak...@vectordatasystems.com
> office: (301) 358-1690 x36
> http://www.vectordatasystems.com
>
>
> Tom DeReggi wrote:
>> While on the topic of generators.
>>
>> Anyone have advice on how to accommodate generators in Commercial
>> Multi-tenant buildings.
>>
>> Several things come to mind... Gas generators are definately not allowed 
>> on
>> roofs, for fire safety reasons.
>> Adequate ventilation is likely needed for either gas or Propain 
>> generators.
>>
>> What type propain generators would likely gain permission to get 
>> installed
>> in a rooftop penthouse? or Roof?
>>
>> If a propain generator was used on a top floor, how would Propain get
>> re-fueled easilly?
>> Is is standard proceedure to have removable tanks, and just have new 
>> tanks
>> swapped (like a gas grill).?
>> Or is is customary to have tanks on the ground level?
>> Or is it always standard to put the generator at ground level, and run AC
>> wire up 

Re: [WISPA] Small auto start generator

2009-08-03 Thread jp
The tripplite APS is what we use for this. Small generators are a pain.

On Sun, Aug 02, 2009 at 02:57:23PM -0430, os10ru...@gmail.com wrote:
> You might want something like an inverter (Xantrex for example) which  
> includes a DC to AC inverter, battery charger, and automatic transfer  
> switch. Add the batteries and you're done.
> 
> Greg
> 
> On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:
> 
> > Thank you,
> > That is very good advice. After some research, I'm leaning toward a  
> > UPS.
> >
> > A pair of good AGM batteries and charge controller will cost less  
> > and be far less maintainence. Then I'd just run the CMM off the  
> > batteries @ 24VDC.
> >
> > Thanks again
> > Jerry
> >
> >
> > -Original Message-
> > From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]  
> > On Behalf Of Gary Garrett
> > Sent: Sunday, August 02, 2009 11:59 AM
> > To: WISPA General List
> > Subject: Re: [WISPA] Small auto start generator
> >
> > Small generators do not auto start very reliably.
> > When cold or dampness causes hard starting the starter can overheat  
> > and
> > burn out. Generally you need an electric choke to start gas engines,
> > propane can "flood" and need to rest before trying again, diesel can  
> > be
> > REAL hard to start when cold. Auto starters can not adapt to changing
> > conditions.
> > Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase.  
> > (1955
> > Model)
> > The monitor cranks for 1 min then rests and tries 3 times.  
> > Everything is
> > adjustable. It knows to stop cranking when it sees AC voltage from the
> > Gen. so the motor over runs the starter for just a few seconds. Only a
> > huge starter motor can take this abuse and last unattended.
> >
> > You may be money ahead to find out why the existing generator is not
> > starting and get it fixed.
> >
> > Jerry Richardson wrote:
> >> We rent on a tower that is suspposed to have gen-set backup but it  
> >> does not start reliably.
> >>
> >> Any recommendations on a small auto-start generator? We only need  
> >> to power a CMMmicro - ~100watts.
> >>
> >> Thanks
> >>
> >>
> >>
> >> __
> >> Jerry Richardson
> >> airCloud Communications
> >>
> >>
> >>
> >>
> >> 
> >> WISPA Wants You! Join today!
> >> http://signup.wispa.org/
> >> 
> >>
> >> WISPA Wireless List: wireless@wispa.org
> >>
> >> Subscribe/Unsubscribe:
> >> http://lists.wispa.org/mailman/listinfo/wireless
> >>
> >> Archives: http://lists.wispa.org/pipermail/wireless/
> >>
> >
> >
> > 
> > WISPA Wants You! Join today!
> > http://signup.wispa.org/
> > 
> >
> > WISPA Wireless List: wireless@wispa.org
> >
> > Subscribe/Unsubscribe:
> > http://lists.wispa.org/mailman/listinfo/wireless
> >
> > Archives: http://lists.wispa.org/pipermail/wireless/
> >
> >
> > 
> > WISPA Wants You! Join today!
> > http://signup.wispa.org/
> > 
> >
> > WISPA Wireless List: wireless@wispa.org
> >
> > Subscribe/Unsubscribe:
> > http://lists.wispa.org/mailman/listinfo/wireless
> >
> > Archives: http://lists.wispa.org/pipermail/wireless/
> 
> 
> 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
> 
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
> 
> Archives: http://lists.wispa.org/pipermail/wireless/

-- 
/*
Jason Philbrook   |   Midcoast Internet Solutions - Wireless and DSL
KB1IOJ|   Broadband Internet Access, Dialup, and Hosting 
 http://f64.nu/   |   for Midcoast Mainehttp://www.midcoast.com/
*/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-03 Thread Marlon K. Schafer
They'll charge a car.  Those have some load on them when just sitting

I'd say that those questions would be best asked of the manufacturer you 
plan to use.

marlon

- Original Message - 
From: "Scott Carullo" 
To: "WISPA General List" 
Sent: Sunday, August 02, 2009 5:05 PM
Subject: Re: [WISPA] Small auto start generator


> Can you use a battery charger to essentially run your load from?
>
> Also will that load cause a smart charger to act not so smart because
> of the load on it?
>
> Scott Carullo
> Brevard Wireless
> (321) 205-1100 x102
>
> On Aug 2, 2009, at 4:30 PM, "Marlon K. Schafer" 
> wrote:
>
>> How long do you need to power it for?
>>
>> I'd suggest that this may be a great case for a couple of big
>> batteries and
>> an inverter.  Just run the system off of the inverter all of the time,
>> install a smart battery charger to keep the batteries properly
>> charged.
>>
>> Cheaper than a generator, NO switch time.  Ever.
>>
>> laters,
>> marlon
>>
>> - Original Message -
>> From: "Jerry Richardson" 
>> To: "Motorola Canopy User Group" ; "WISPA
>> General List"
>> 
>> Sent: Sunday, August 02, 2009 11:34 AM
>> Subject: [WISPA] Small auto start generator
>>
>>
>>> We rent on a tower that is suspposed to have gen-set backup but it
>>> does
>>> not start reliably.
>>>
>>> Any recommendations on a small auto-start generator? We only need
>>> to power
>>> a CMMmicro - ~100watts.
>>>
>>> Thanks
>>>
>>>
>>>
>>> __
>>> Jerry Richardson
>>> airCloud Communications
>>>
>>>
>>>
>>>
>>> --- 
>>> --- 
>>> --- 
>>> --- 
>>> 
>>> WISPA Wants You! Join today!
>>> http://signup.wispa.org/
>>> --- 
>>> --- 
>>> --- 
>>> --- 
>>> 
>>>
>>> WISPA Wireless List: wireless@wispa.org
>>>
>>> Subscribe/Unsubscribe:
>>> http://lists.wispa.org/mailman/listinfo/wireless
>>>
>>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>>
>>
>> --- 
>> --- 
>> --- 
>> --- 
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> --- 
>> --- 
>> --- 
>> --- 
>> 
>>
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/ 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-03 Thread Patrick Shoemaker
Yes, it's possible to get a generator installed on a roof, but it will 
be an expensive project in our area due to the code compliance issues. 
However, most commercial buildings will have a preexisting emergency 
power system for critical loads installed already. There are strict 
requirements such as sub 10 second startup times, routine testing, and 
fuel availability requirements. If you talk to the building engineer, 
you might be able to convince them to allow you a small amount of power 
from an emergency circuit. The buildings I am in do this for most of 
their tenants for phone systems, etc.

Failing that, have an electrician run conduit to the parking lot and 
place a power inlet down there. Be sure to have 24 hours of battery 
capacity, and use a trailer-mounted generator in the parking lot for the 
rare outage that lasts longer than the batteries.


Patrick Shoemaker
Vector Data Systems LLC
shoemak...@vectordatasystems.com
office: (301) 358-1690 x36
http://www.vectordatasystems.com


Tom DeReggi wrote:
> While on the topic of generators.
> 
> Anyone have advice on how to accommodate generators in Commercial 
> Multi-tenant buildings.
> 
> Several things come to mind... Gas generators are definately not allowed on 
> roofs, for fire safety reasons.
> Adequate ventilation is likely needed for either gas or Propain generators.
> 
> What type propain generators would likely gain permission to get installed 
> in a rooftop penthouse? or Roof?
> 
> If a propain generator was used on a top floor, how would Propain get 
> re-fueled easilly?
> Is is standard proceedure to have removable tanks, and just have new tanks 
> swapped (like a gas grill).?
> Or is is customary to have tanks on the ground level?
> Or is it always standard to put the generator at ground level, and run AC 
> wire up to the roof level?
> Do propain gas trucks have long enough hoses to reach rooms inside parking 
> garages? Not likely will fit driving into parking garage?
> 
> Do property owners worry about propain blowing up, and have limits to where 
> the tanks can be placed?
> 
> I'm sure some of this is in local building code.  And I can probably best 
> guess some of the answers for above.
> 
> But what re other people doing, to both install and maintain at the lowest 
> dollar cost.?
> 
> I saw those Generac propain models before, and they are very affordable. 
> Just wondering if feasible to install them on roofs/penthouses.
> 
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
> 
> 
> ----- Original Message ----- 
> From: "Jerry Richardson" 
> To: "WISPA General List" 
> Sent: Sunday, August 02, 2009 3:08 PM
> Subject: Re: [WISPA] Small auto start generator
> 
> 
>> Thank you,
>> That is very good advice. After some research, I'm leaning toward a UPS.
>>
>> A pair of good AGM batteries and charge controller will cost less and be 
>> far less maintainence. Then I'd just run the CMM off the batteries @ 
>> 24VDC.
>>
>> Thanks again
>> Jerry
>>
>>
>> -Original Message-
>> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On 
>> Behalf Of Gary Garrett
>> Sent: Sunday, August 02, 2009 11:59 AM
>> To: WISPA General List
>> Subject: Re: [WISPA] Small auto start generator
>>
>> Small generators do not auto start very reliably.
>> When cold or dampness causes hard starting the starter can overheat and
>> burn out. Generally you need an electric choke to start gas engines,
>> propane can "flood" and need to rest before trying again, diesel can be
>> REAL hard to start when cold. Auto starters can not adapt to changing
>> conditions.
>> Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955
>> Model)
>> The monitor cranks for 1 min then rests and tries 3 times. Everything is
>> adjustable. It knows to stop cranking when it sees AC voltage from the
>> Gen. so the motor over runs the starter for just a few seconds. Only a
>> huge starter motor can take this abuse and last unattended.
>>
>> You may be money ahead to find out why the existing generator is not
>> starting and get it fixed.
>>
>> Jerry Richardson wrote:
>>> We rent on a tower that is suspposed to have gen-set backup but it does 
>>> not start reliably.
>>>
>>> Any recommendations on a small auto-start generator? We only need to 
>>> power a CMMmicro - ~100watts.
>>>
>>> Thanks
>>>
>>>
>>>
>>> __

Re: [WISPA] Small auto start generator

2009-08-02 Thread os10rules
There are chargers such as the Iota batter charger/power supply 
http://www.iotaengineering.com/dls.htm 
  which are clean enough to run directly off of even with no battery.  
With a battery the battery just floats (no current in or out) as long  
as the battery charger is supplied AC. Once the AC drops the system  
runs off the battery. When power returns the Iota charger charges the  
battery and supplies power to the load till the battery is charged and  
then it just floats again.

Greg
On Aug 2, 2009, at 7:35 PM, Scott Carullo wrote:

> Can you use a battery charger to essentially run your load from?
>
> Also will that load cause a smart charger to act not so smart because
> of the load on it?
>
> Scott Carullo
> Brevard Wireless
> (321) 205-1100 x102
>
> On Aug 2, 2009, at 4:30 PM, "Marlon K. Schafer" 
> wrote:
>
>> How long do you need to power it for?
>>
>> I'd suggest that this may be a great case for a couple of big
>> batteries and
>> an inverter.  Just run the system off of the inverter all of the  
>> time,
>> install a smart battery charger to keep the batteries properly
>> charged.
>>
>> Cheaper than a generator, NO switch time.  Ever.
>>
>> laters,
>> marlon
>>
>> - Original Message -
>> From: "Jerry Richardson" 
>> To: "Motorola Canopy User Group" ; "WISPA
>> General List"
>> 
>> Sent: Sunday, August 02, 2009 11:34 AM
>> Subject: [WISPA] Small auto start generator
>>
>>
>>> We rent on a tower that is suspposed to have gen-set backup but it
>>> does
>>> not start reliably.
>>>
>>> Any recommendations on a small auto-start generator? We only need
>>> to power
>>> a CMMmicro - ~100watts.
>>>
>>> Thanks
>>>
>>>
>>>
>>> __
>>> Jerry Richardson
>>> airCloud Communications
>>>
>>>
>>>
>>>
>>> ---
>>> ---
>>> ---
>>> ---
>>> 
>>> WISPA Wants You! Join today!
>>> http://signup.wispa.org/
>>> ---
>>> ---
>>> ---
>>> ---
>>> 
>>>
>>> WISPA Wireless List: wireless@wispa.org
>>>
>>> Subscribe/Unsubscribe:
>>> http://lists.wispa.org/mailman/listinfo/wireless
>>>
>>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>>
>>
>> ---
>> ---
>> ---
>> ---
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> ---
>> ---
>> ---
>> ---
>> 
>>
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread Josh Luthman
Generators are not illegal on roof tops.  The once-hospital here has an
enormous diesel one straight above me!  It is now a multi-tenant building
for businesses and residents.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

"When you have eliminated the impossible, that which remains, however
improbable, must be the truth."
--- Sir Arthur Conan Doyle


On Sun, Aug 2, 2009 at 10:29 PM, Tom DeReggi wrote:

> While on the topic of generators.
>
> Anyone have advice on how to accommodate generators in Commercial
> Multi-tenant buildings.
>
> Several things come to mind... Gas generators are definately not allowed on
> roofs, for fire safety reasons.
> Adequate ventilation is likely needed for either gas or Propain generators.
>
> What type propain generators would likely gain permission to get installed
> in a rooftop penthouse? or Roof?
>
> If a propain generator was used on a top floor, how would Propain get
> re-fueled easilly?
> Is is standard proceedure to have removable tanks, and just have new tanks
> swapped (like a gas grill).?
> Or is is customary to have tanks on the ground level?
> Or is it always standard to put the generator at ground level, and run AC
> wire up to the roof level?
> Do propain gas trucks have long enough hoses to reach rooms inside parking
> garages? Not likely will fit driving into parking garage?
>
> Do property owners worry about propain blowing up, and have limits to where
> the tanks can be placed?
>
> I'm sure some of this is in local building code.  And I can probably best
> guess some of the answers for above.
>
> But what re other people doing, to both install and maintain at the lowest
> dollar cost.?
>
> I saw those Generac propain models before, and they are very affordable.
> Just wondering if feasible to install them on roofs/penthouses.
>
> Tom DeReggi
> RapidDSL & Wireless, Inc
> IntAirNet- Fixed Wireless Broadband
>
>
> ----- Original Message -----
> From: "Jerry Richardson" 
> To: "WISPA General List" 
> Sent: Sunday, August 02, 2009 3:08 PM
> Subject: Re: [WISPA] Small auto start generator
>
>
> > Thank you,
> > That is very good advice. After some research, I'm leaning toward a UPS.
> >
> > A pair of good AGM batteries and charge controller will cost less and be
> > far less maintainence. Then I'd just run the CMM off the batteries @
> > 24VDC.
> >
> > Thanks again
> > Jerry
> >
> >
> > -Original Message-
> > From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
> > Behalf Of Gary Garrett
> > Sent: Sunday, August 02, 2009 11:59 AM
> > To: WISPA General List
> > Subject: Re: [WISPA] Small auto start generator
> >
> > Small generators do not auto start very reliably.
> > When cold or dampness causes hard starting the starter can overheat and
> > burn out. Generally you need an electric choke to start gas engines,
> > propane can "flood" and need to rest before trying again, diesel can be
> > REAL hard to start when cold. Auto starters can not adapt to changing
> > conditions.
> > Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955
> > Model)
> > The monitor cranks for 1 min then rests and tries 3 times. Everything is
> > adjustable. It knows to stop cranking when it sees AC voltage from the
> > Gen. so the motor over runs the starter for just a few seconds. Only a
> > huge starter motor can take this abuse and last unattended.
> >
> > You may be money ahead to find out why the existing generator is not
> > starting and get it fixed.
> >
> > Jerry Richardson wrote:
> >> We rent on a tower that is suspposed to have gen-set backup but it does
> >> not start reliably.
> >>
> >> Any recommendations on a small auto-start generator? We only need to
> >> power a CMMmicro - ~100watts.
> >>
> >> Thanks
> >>
> >>
> >>
> >> __
> >> Jerry Richardson
> >> airCloud Communications
> >>
> >>
> >>
> >>
> >>
> 
> >> WISPA Wants You! Join today!
> >> http://signup.wispa.org/
> >>
> 
> >>
> >> WISPA Wireless List: wireless@wispa.org
> >>
> >> Subscribe/Unsubscribe:
> >> http://lists.wispa.org/mailman/listinfo/wireless
> >>

Re: [WISPA] Small auto start generator

2009-08-02 Thread Tom DeReggi
While on the topic of generators.

Anyone have advice on how to accommodate generators in Commercial 
Multi-tenant buildings.

Several things come to mind... Gas generators are definately not allowed on 
roofs, for fire safety reasons.
Adequate ventilation is likely needed for either gas or Propain generators.

What type propain generators would likely gain permission to get installed 
in a rooftop penthouse? or Roof?

If a propain generator was used on a top floor, how would Propain get 
re-fueled easilly?
Is is standard proceedure to have removable tanks, and just have new tanks 
swapped (like a gas grill).?
Or is is customary to have tanks on the ground level?
Or is it always standard to put the generator at ground level, and run AC 
wire up to the roof level?
Do propain gas trucks have long enough hoses to reach rooms inside parking 
garages? Not likely will fit driving into parking garage?

Do property owners worry about propain blowing up, and have limits to where 
the tanks can be placed?

I'm sure some of this is in local building code.  And I can probably best 
guess some of the answers for above.

But what re other people doing, to both install and maintain at the lowest 
dollar cost.?

I saw those Generac propain models before, and they are very affordable. 
Just wondering if feasible to install them on roofs/penthouses.

Tom DeReggi
RapidDSL & Wireless, Inc
IntAirNet- Fixed Wireless Broadband


- Original Message - 
From: "Jerry Richardson" 
To: "WISPA General List" 
Sent: Sunday, August 02, 2009 3:08 PM
Subject: Re: [WISPA] Small auto start generator


> Thank you,
> That is very good advice. After some research, I'm leaning toward a UPS.
>
> A pair of good AGM batteries and charge controller will cost less and be 
> far less maintainence. Then I'd just run the CMM off the batteries @ 
> 24VDC.
>
> Thanks again
> Jerry
>
>
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On 
> Behalf Of Gary Garrett
> Sent: Sunday, August 02, 2009 11:59 AM
> To: WISPA General List
> Subject: Re: [WISPA] Small auto start generator
>
> Small generators do not auto start very reliably.
> When cold or dampness causes hard starting the starter can overheat and
> burn out. Generally you need an electric choke to start gas engines,
> propane can "flood" and need to rest before trying again, diesel can be
> REAL hard to start when cold. Auto starters can not adapt to changing
> conditions.
> Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955
> Model)
> The monitor cranks for 1 min then rests and tries 3 times. Everything is
> adjustable. It knows to stop cranking when it sees AC voltage from the
> Gen. so the motor over runs the starter for just a few seconds. Only a
> huge starter motor can take this abuse and last unattended.
>
> You may be money ahead to find out why the existing generator is not
> starting and get it fixed.
>
> Jerry Richardson wrote:
>> We rent on a tower that is suspposed to have gen-set backup but it does 
>> not start reliably.
>>
>> Any recommendations on a small auto-start generator? We only need to 
>> power a CMMmicro - ~100watts.
>>
>> Thanks
>>
>>
>>
>> __
>> Jerry Richardson
>> airCloud Communications
>>
>>
>>
>>
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> 
>>
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/ 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread Scott Carullo
Can you use a battery charger to essentially run your load from?

Also will that load cause a smart charger to act not so smart because  
of the load on it?

Scott Carullo
Brevard Wireless
(321) 205-1100 x102

On Aug 2, 2009, at 4:30 PM, "Marlon K. Schafer"   
wrote:

> How long do you need to power it for?
>
> I'd suggest that this may be a great case for a couple of big  
> batteries and
> an inverter.  Just run the system off of the inverter all of the time,
> install a smart battery charger to keep the batteries properly  
> charged.
>
> Cheaper than a generator, NO switch time.  Ever.
>
> laters,
> marlon
>
> - Original Message -
> From: "Jerry Richardson" 
> To: "Motorola Canopy User Group" ; "WISPA  
> General List"
> 
> Sent: Sunday, August 02, 2009 11:34 AM
> Subject: [WISPA] Small auto start generator
>
>
>> We rent on a tower that is suspposed to have gen-set backup but it  
>> does
>> not start reliably.
>>
>> Any recommendations on a small auto-start generator? We only need  
>> to power
>> a CMMmicro - ~100watts.
>>
>> Thanks
>>
>>
>>
>> __
>> Jerry Richardson
>> airCloud Communications
>>
>>
>>
>>
>> --- 
>> --- 
>> --- 
>> --- 
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> --- 
>> --- 
>> --- 
>> --- 
>> 
>>
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
>
> --- 
> --- 
> --- 
> --- 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> --- 
> --- 
> --- 
> --- 
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread Leon D. Zetekoff, NCE
Hi Guys...I'd steer away from inverters since they soak up a lot of 
power. You might want to look at some solar stuff with some of the AGM 
batteries Marlon mentioned in another thread. Run everything @ 24V is 
good that way you don't need any dc-dc converters.


Leon

* os10ru...@gmail.com wrote, On 8/2/2009 3:27 PM:
You might want something like an inverter (Xantrex for example) which  
includes a DC to AC inverter, battery charger, and automatic transfer  
switch. Add the batteries and you're done.


Greg

On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:

  

Thank you,
That is very good advice. After some research, I'm leaning toward a  
UPS.


A pair of good AGM batteries and charge controller will cost less  
and be far less maintainence. Then I'd just run the CMM off the  
batteries @ 24VDC.


Thanks again
Jerry


-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]  
On Behalf Of Gary Garrett

Sent: Sunday, August 02, 2009 11:59 AM
To: WISPA General List
Subject: Re: [WISPA] Small auto start generator

Small generators do not auto start very reliably.
When cold or dampness causes hard starting the starter can overheat  
and

burn out. Generally you need an electric choke to start gas engines,
propane can "flood" and need to rest before trying again, diesel can  
be

REAL hard to start when cold. Auto starters can not adapt to changing
conditions.
Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase.  
(1955

Model)
The monitor cranks for 1 min then rests and tries 3 times.  
Everything is

adjustable. It knows to stop cranking when it sees AC voltage from the
Gen. so the motor over runs the starter for just a few seconds. Only a
huge starter motor can take this abuse and last unattended.

You may be money ahead to find out why the existing generator is not
starting and get it fixed.

Jerry Richardson wrote:

We rent on a tower that is suspposed to have gen-set backup but it  
does not start reliably.


Any recommendations on a small auto-start generator? We only need  
to power a CMMmicro - ~100watts.


Thanks

__
Jerry Richardson
airCloud Communications
  

No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.5.406 / Virus Database: 270.13.42/2278 - Release Date: 08/02/09 
17:56:00



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Small auto start generator

2009-08-02 Thread Marlon K. Schafer
How long do you need to power it for?

I'd suggest that this may be a great case for a couple of big batteries and 
an inverter.  Just run the system off of the inverter all of the time, 
install a smart battery charger to keep the batteries properly charged.

Cheaper than a generator, NO switch time.  Ever.

laters,
marlon

- Original Message - 
From: "Jerry Richardson" 
To: "Motorola Canopy User Group" ; "WISPA General List" 

Sent: Sunday, August 02, 2009 11:34 AM
Subject: [WISPA] Small auto start generator


> We rent on a tower that is suspposed to have gen-set backup but it does 
> not start reliably.
>
> Any recommendations on a small auto-start generator? We only need to power 
> a CMMmicro - ~100watts.
>
> Thanks
>
>
>
> __
> Jerry Richardson
> airCloud Communications
>
>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/ 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread os10rules
You might want something like an inverter (Xantrex for example) which  
includes a DC to AC inverter, battery charger, and automatic transfer  
switch. Add the batteries and you're done.

Greg

On Aug 2, 2009, at 2:38 PM, Jerry Richardson wrote:

> Thank you,
> That is very good advice. After some research, I'm leaning toward a  
> UPS.
>
> A pair of good AGM batteries and charge controller will cost less  
> and be far less maintainence. Then I'd just run the CMM off the  
> batteries @ 24VDC.
>
> Thanks again
> Jerry
>
>
> -Original Message-
> From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org]  
> On Behalf Of Gary Garrett
> Sent: Sunday, August 02, 2009 11:59 AM
> To: WISPA General List
> Subject: Re: [WISPA] Small auto start generator
>
> Small generators do not auto start very reliably.
> When cold or dampness causes hard starting the starter can overheat  
> and
> burn out. Generally you need an electric choke to start gas engines,
> propane can "flood" and need to rest before trying again, diesel can  
> be
> REAL hard to start when cold. Auto starters can not adapt to changing
> conditions.
> Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase.  
> (1955
> Model)
> The monitor cranks for 1 min then rests and tries 3 times.  
> Everything is
> adjustable. It knows to stop cranking when it sees AC voltage from the
> Gen. so the motor over runs the starter for just a few seconds. Only a
> huge starter motor can take this abuse and last unattended.
>
> You may be money ahead to find out why the existing generator is not
> starting and get it fixed.
>
> Jerry Richardson wrote:
>> We rent on a tower that is suspposed to have gen-set backup but it  
>> does not start reliably.
>>
>> Any recommendations on a small auto-start generator? We only need  
>> to power a CMMmicro - ~100watts.
>>
>> Thanks
>>
>>
>>
>> __
>> Jerry Richardson
>> airCloud Communications
>>
>>
>>
>>
>> 
>> WISPA Wants You! Join today!
>> http://signup.wispa.org/
>> 
>>
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/
>
>
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>
> WISPA Wireless List: wireless@wispa.org
>
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
>
> Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread Jerry Richardson
Thank you,
That is very good advice. After some research, I'm leaning toward a UPS. 

A pair of good AGM batteries and charge controller will cost less and be far 
less maintainence. Then I'd just run the CMM off the batteries @ 24VDC.

Thanks again
Jerry


-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On Behalf 
Of Gary Garrett
Sent: Sunday, August 02, 2009 11:59 AM
To: WISPA General List
Subject: Re: [WISPA] Small auto start generator

Small generators do not auto start very reliably.
When cold or dampness causes hard starting the starter can overheat and 
burn out. Generally you need an electric choke to start gas engines, 
propane can "flood" and need to rest before trying again, diesel can be 
REAL hard to start when cold. Auto starters can not adapt to changing 
conditions.
Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955 
Model)
The monitor cranks for 1 min then rests and tries 3 times. Everything is 
adjustable. It knows to stop cranking when it sees AC voltage from the 
Gen. so the motor over runs the starter for just a few seconds. Only a 
huge starter motor can take this abuse and last unattended.

You may be money ahead to find out why the existing generator is not 
starting and get it fixed.

Jerry Richardson wrote:
> We rent on a tower that is suspposed to have gen-set backup but it does not 
> start reliably.
> 
> Any recommendations on a small auto-start generator? We only need to power a 
> CMMmicro - ~100watts.
> 
> Thanks
> 
> 
> 
> __
> Jerry Richardson
> airCloud Communications
> 
> 
> 
> 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
> 
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
> 
> Archives: http://lists.wispa.org/pipermail/wireless/
> 



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread Gary Garrett
Small generators do not auto start very reliably.
When cold or dampness causes hard starting the starter can overheat and 
burn out. Generally you need an electric choke to start gas engines, 
propane can "flood" and need to rest before trying again, diesel can be 
REAL hard to start when cold. Auto starters can not adapt to changing 
conditions.
Our best generator is a Propane Ford inline 6 cyl. 25 KW 3 phase. (1955 
Model)
The monitor cranks for 1 min then rests and tries 3 times. Everything is 
adjustable. It knows to stop cranking when it sees AC voltage from the 
Gen. so the motor over runs the starter for just a few seconds. Only a 
huge starter motor can take this abuse and last unattended.

You may be money ahead to find out why the existing generator is not 
starting and get it fixed.

Jerry Richardson wrote:
> We rent on a tower that is suspposed to have gen-set backup but it does not 
> start reliably.
> 
> Any recommendations on a small auto-start generator? We only need to power a 
> CMMmicro - ~100watts.
> 
> Thanks
> 
> 
> 
> __
> Jerry Richardson
> airCloud Communications
> 
> 
> 
> 
> 
> WISPA Wants You! Join today!
> http://signup.wispa.org/
> 
>  
> WISPA Wireless List: wireless@wispa.org
> 
> Subscribe/Unsubscribe:
> http://lists.wispa.org/mailman/listinfo/wireless
> 
> Archives: http://lists.wispa.org/pipermail/wireless/
> 



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Small auto start generator

2009-08-02 Thread eje
Way more then what you need. 

http://www.homedepot.com/webapp/wcs/stores/servlet/ProductDisplay?storeId=10051&langId=-1&catalogId=10053&productId=100628959&categoryID=524799

The generac works great. Not sure if you have nural gas there but they can also 
be converted to propane. 

/Eje
--Original Message--
From: Jerry Richardson
Sender: wireless-boun...@wispa.org
To: Motorola Canopy User Group
To: WISPA General List
ReplyTo: WISPA General List
Subject: [WISPA] Small auto start generator
Sent: Aug 2, 2009 13:34

We rent on a tower that is suspposed to have gen-set backup but it does not 
start reliably.

Any recommendations on a small auto-start generator? We only need to power a 
CMMmicro - ~100watts.

Thanks



__
Jerry Richardson
airCloud Communications





WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Sent via BlackBerry from T-Mobile



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/