enough air. You didn't mention gen set model, or
whether the frequency was a solid 60 hz. I've seen bad things happen
when the frequency got out of spec too. I'm guessing a bad voltage
regulator on the gen set.
Ray Walters
Remote Solar
On 4/25/2024 11:24 AM, Kevin Pegg via RE-wrenches wrote
. The
cheapo BMS lears its ugly head once again. All we're doing lately is
fixing stuff less than 5 years old.
Ray Walters
Remote Solar
On 4/25/2024 9:52 AM, Michael Morningstar via RE-wrenches wrote:
Here's a different take. Just food for thought and not necessarily a
suggestion. Those 1st
and the customer can be
bored for a decade. It will make more power too, especially on cold,
sunny days when you really need it.
Ray Walters
Remote Solar
On 4/23/2024 12:47 PM, Todd Cory via RE-wrenches wrote:
My old MX60 said " hot" when the fan had failed.
Todd
"MX 2 Hot (Very rare)
it in house to pencil out. I'm not sure if it ever would,
considering that you still have to pay yourself or someone else to
operate the engraver, and the blank plaques probably cost a bit too.
Ray Walters
Remote Solar
On 3/30/2024 12:56 PM, Lou Russo via RE-wrenches wrote:
Aloha Wrenches,
Anyone
applications. The rest of us in the other 49 states are Not required
to comply with the 200 A requirement.
Good Luck out there.
Thank you,
Ray Walters
Remote Solar
On 3/28/2024 12:33 PM, Lloyd Hoffstatter via RE-wrenches wrote:
William,
Here is the CA Energy Code with the upsized busbar
xception 1 specifically says a single N-G bond is allowed for multiple
power sources.
Ray Walters
Remote Solar
On 3/13/2024 3:19 PM, Mick Abraham via RE-wrenches wrote:
Hi, Mechanix~
My off grid project gig has redundant 120y208 generators that need a
200a "break before make" manua
for, and I sleep well at
night with my standard contractor's liability insurance.
Remember, insurance agents primary goal is to sell more insurance. Of
course they want you to have an E policy, too.
Ray Walters
Remote Solar
On 3/11/2024 7:41 PM, Howie Michaelson via RE-wrenches wrote:
William, et
down mounting, and no losses. I've been
suspicious of top down module racking; and I was quite satisfied with
actual bolts and hardware to hold modules in place. But its just not
true anymore. I added 3/4" angle stainless steel to reinforce the
attachments on the top modules.
Ray Walters
On
Here's another mount at the edge of failure, from the same system.
Hardware is tight. Like many, I had lots of love for good ol' fashion
bottom mounting vs top mount, until this happened about 5 years ago.
This is how we learn.
On 3/8/2024 5:15 PM, Ray Walters via RE-wrenches wrote:
I've
I've had several modules pull off of bottom mount racking in high winds,
but never top mount racking. Newer modules have much thinner frames,
but are much more surface area than the old days.
So to answer Kent's question:
Ray Walters
Remote Solar
On 3/8/2024 3:50 PM, Kent via RE-wrenches
that's quite
accurate; I tried it on some bottles with fluid in them, and it seemed
to work well. I'll try and remember to take out with me on the next job
with FLA.
Ray Walters
Remote Solar
On 2/29/2024 2:12 PM, William Miller via RE-wrenches wrote:
Friends:
Thanks to everyone who responded
Who carries the Superwind turbines? We've been looking for a
replacement for the old Bergey XL1 to offer clients.
Thanks,
Ray Walters
Remote Solar
On 2/21/2024 7:20 PM, John Blittersdorf via RE-wrenches wrote:
As far as wind is concerned, I recommend SuperWind, made in Germany.
It is well
like "lead acid batteries aren't allowed", will get them to
back down on the spot. Getting solar trade organizations on your side
to help with the process can add much needed weight.
Ray Walters
Remote Solar
On 2/17/2024 2:26 PM, Dan Fink via RE-wrenches wrote:
Jay - Despite the excepti
ere.
Also, with all the mention of various UL listings, regulation needs to
evolve to differentiate between LiFePO4 and other Li+ chemistries.
LiFePO4 is inherently much safer, but we're being forced to comply with
all the same regulations as the less stable, more energy dense chemistries.
R
I second using the 48v to 12 v DC DC converter. I've had success with
that, and avoided the issues Jeremy mentioned.
Ray Walters
Remote Solar
On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote:
I powered a MidNite LSOB transmitter from a Classic AUX, though the
receivers didn't work
What's funny, is the good old SWs from the Trace days had the same
problem. Never could get them to equalize. Maybe that software
carried over.
Ray Walters
Remote Solar
On 2/12/2024 4:42 PM, jay via RE-wrenches wrote:
Hi Kevin
Thanks, I heard that exact thing from someone else.
Do you
Hi Richard;
Off list, what was your outcome from Simpliphi? Did they make any deal
with you? What did you put in as replacements?
Thanks,
Ray Walters
Remote Solar
On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote:
Hi Ray
We had a complete failure of 6 Simpliphi batteries
ng for SLA batteries to get this
customer back in action.
Reporting as always from the Bleeding Edge,
Ray Walters
Remote Solar
On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote:
Hi Ray
We had a complete failure of 6 Simpliphi batteries with the same
symptoms you found.
Another ins
of these high price tag batteries
don't start failing on my watch.
I've been holding this rant back for a while, trying to give Simpliphi a
chance to make this right. However, this week I heard their "diagnosis",
and then I saw Jay's timely post? I knew it was time.
Sincerely,
R
I'm trying to find a pic to post, but they were MC4 connectors, not the UTX.
Ray
On 11/9/2023 4:57 PM, Brian Mehalic wrote:
Are they the Amohenol UTX connectors? SW had a recall on them, sounds
like about the right timeframe.
BREAKING: SolarWorld recalls PV modules with Amphenol connectors
connector type.
10+ amps continuous, moist environment, 30F+ hotter than ambient temp,
all are tough on connectors. I predict more connector failures as
module current ratings increase.
Ray Walters
Remote Solar
On 11/9/2023 3:02 PM, Glenn Burt via RE-wrenches wrote:
Good luck trying to con
What is the array size vs the battery size? Sounds like a big array on
a small battery for the voltage to go that high that fast.
Ray
Remote Solar
On 10/21/2023 5:46 PM, William Miller via RE-wrenches wrote:
Friends:
I’m kinda stuck on a project setting up a SI/SB AC coupled system off
s? Definitely needs to be in a metal
enclosure.
I think its either get a different washer or get a different inverter.
At 22+ years, its slowly reaching the time to retire those old SWs.
Ray Walters
Remote Solar
303 505-8760
On 9/8/23 2:53 PM, Dave Angelini Offgrid Solar via RE-wrenches wrot
, which is what many folks find attractive,
I think.
Ray Walters
On 8/17/2023 1:41 PM, Jay via RE-wrenches wrote:
Im curious if anyone has actual measured data on a VAWT.
It just seems like they are meat for the end of the worlders
Jay
___
List
manually turn the
inverters back on.
Ray
On 7/20/2023 5:15 PM, Jay wrote:
Hi Ray
This house won’t have an AGS, manual start only.
And your comments exactly, having to wait until the next day when
hopefully there is enough sun to charge the battery is iffy.
Or they could do the inverter bypass
The aux off is only if the generator doesn't start. You need to set the
gen start voltage higher. Aux off is last ditch shut down, set for 44v
for lead acid, or 47 to 49v, depending on the battery and inverter.
Hopefully DC coupled PV will raise the voltage enough to turn the
inverters back
brand BTW.
Ray Walters
On 7/16/2023 4:18 PM, Kent via RE-wrenches wrote:
I think these modules are about 12 years old. I didn't have a
voltmeter or ammeter with me this morning when this was discovered so
I wasn't able to check the output.
Kent Osterberg
Blue Mountain Solar
On 7/16/2023 3:06
. Absolutely makes no
sense. Schneider, Outback, even Magnum is too low...?
Ray Walters
On 7/11/2023 6:19 PM, Mac Lewis via RE-wrenches wrote:
Hello Wrenches,
I'm trying to solve an issue with an older Outback FX system. It's a
quad stack of Outback 3648 FX inverters and he has a couple
of the driver circuits on
the LED bulbs. Only gets worse on a less than perfect AC waveform.
Ray Walters
Remote Solar
On 7/3/2023 5:09 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
I think I would try eliminating things. Turn off the AC coupling for a
few days and get results. Turn
. That sounds more like a cooked control board. I had
lightning damage cause an inverter to put out 140 vac, while its onboard
electronics read 120 vac.
If it helps, I have a used MS 4024 PAE (very low hours) that I could
send to you. Contact me off list if you want.
Ray Walters
Remote Solar
g off grid, and the only thing better than a Magnum for power
quality is Exeltech in my experience.
Ray Walters
Remote Solar
On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote:
Hi all,
I have a client with a Magnum MS 4024- PAE inverter. There are some
serious issues with power outp
production on the PV system, and then do some subtraction.
Pretty simple for them, and you only get a call, if the inverter
production is low or off.
Ray Walters
Remote Solar
On 5/11/2023 2:20 PM, Larry Brown via RE-wrenches wrote:
Does anyone have a recommendation for a high quality meter
looked up (just like wire losses) for the size pipe and flow
rate.
Finally, you didn't mention how large a pond. To fill the pond, it
needs to overcome both evaporative losses, and leakage into the
surrounding soil.
Ray Walters
Remote Solar
On 5/8/2023 10:04 AM, Howie Michaelson via RE-wren
If the temperature is right, my IR camera can see the rafters. Best to
check early on a cold morning with the heat on in the building.
Otherwise I'm of the William "Hammer" system persuasion. Never found
anything better.
On 4/17/2023 1:31 PM, Garrison via RE-wrenches wrote:
Hi Kris,
I
on't cheap out.
Ray Walters
Remote Solar
On 4/4/2023 5:42 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
Hurts my head ! Agree that you will have more trips to this house
after the next one. This is most likely not going to get you 2 more
years. All of the wiring is good, clean, and t
the inverters. IF the inverters are Outback, they
have a remote switch, if its something else, you might have to actually
switch off a relay on the AC output.
Ray
On 4/4/2023 2:45 PM, Daniel Young via RE-wrenches wrote:
Thanks all for the advice. I figured it was not worth trying on a
different battery
, I've seen
less than 5 years from sealed L16s like Trojan. Full River is about the
best in that field, and still only going to see 7 to 8 years. It just
doesn't pencil out compared to HUPs or Li+.
Ray Walters
Remote Solar
On 4/3/2023 12:39 PM, William Miller via RE-wrenches wrote:
Daniel:
I
a bit better with
new found idea on each install.
Thanks again for great ideas Wrenches,
Ray
On 3/31/2023 2:15 PM, Jason Szumlanski wrote:
Hi Ray,
I'm happy to have some confirmation from another major storm's impact.
My father has a home in Dominica, which was hit by Maria with 165 mph
winds
Use an electric screw driver, socket wrench, or *drill with a clutch*
set low to snug up the clamps, and then final torque with a torque
wrench. Period.
Ray Walters
Remote Solar
Former NABCEP 2004-2016
On 3/30/2023 4:34 PM, Jason Szumlanski via RE-wrenches wrote:
That would be great if it were pos
th
wiring into the system. Maybe she could do what several folks have
done: power a TV while you pedal. Anyway, here is device that might do
it: https://www.econvergence.net/
Ray Walters
Remote Solar
On 3/16/2023 3:58 PM, Larry Brown via RE-wrenches wrote:
Wrenches
I have a client that we did a
a couple pics of your sprayer install?
2nd question: what are the field results of these systems in actual fires?
Thanks,
Ray
On 3/14/2023 10:03 AM, Todd Cory via RE-wrenches wrote:
I can help with this as Michael built something similar to what I
designed and installed in 2001:
I plumbed
Michael;
Can you share more about your sprinkler system and the power supply for
it? Over the years, at least two of my customers have lost their homes
(and PV arrays) in wild fires.
Ray Walters
Remote Solar
On 3/13/2023 2:34 PM, Michael Morningstar via RE-wrenches wrote:
WebRelay. I use
I'm not an EMP expert by any means, but I've dealt with quite a few
lightning damaged systems. Having a good connection to a low impedance
grounding system (steel cased well, Ufer ground) is crucial. I also
have had fantastic luck with Midnite's MNSPD line. Delta, not so much.
On 3/9/2023
that is in an Hammond organ, so
that I can tune the organ down from A=440 Hz to A =432 Hz to match an
even older piano.Yep, I'm living on the edge..
Ray Walters
(Now Even More) Remote Solar
___
List sponsored by Redwood Alliance
Pay optional
for anything
greater than 60 amps for 2 poles, other than large DPDT switches which
get pricey and hard to source especially for 200 amps?
Howie
On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches
wrote:
I probably still have one of the old QO boxes on the shelf, but I
never liked
://www.northerntool.com/shop/tools/product_200653609_200653609
Midnite makes small 30A and 60A T switches as well:
https://www.midnitesolar.com/productPhoto.php?product_ID=416_ID=29=3=p
Ray Walters
On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote:
Kris, It was SqD QO403, and it was a 3-pole load center
than squeezing an extra 5% capacity out of the battery Notes in the
online instructions such as "/Failure to properly upgrade the firmware
may cause the battery to stop working!", / are not making we want to
push ahead with closed loop either.
Ray
On 2/9/2023 11:01 AM, Chris Sc
with the Solark's
load controls.
I've considered some DC options, but they don't make much sense, since
the inverter has to be on to charge from PV anyway.
The long term plan is for the client to finish the insulation, and sheet
rock, and add a gas wall heater in there as needed.
Thanks,
Ray Walters
bunch of DIY garbage. Find out who did the original wiring.
Probably not a pro.
Ray Walters
Remote Solar
On 12/16/2022 11:35 AM, Kirk Herander via RE-wrenches wrote:
You may have neutral and ground connected at more than 1 location,
meaning at the genset and in house panel, which means the ground
To add to Jeff's suggestion of targeting 95%, many Li+ batteries have a
spike in voltage as they reach 100%. We just don't have to worry
anymore about sulfate damage from under charging.
Ray Walters
Remote Solar
On 11/19/2022 7:14 AM, Jeff Clearwater via RE-wrenches wrote:
Hi Kris
What
, with
built in color touch screen for monitoring, price much better.
Simpliphi = no monitoring at all, have to parallel ridiculous qty of
batteries to do a normal off grid home, but integration guides are the best.
Ray Walters
On 11/17/2022 1:16 PM, r...@solartechvt.com wrote:
We’ve started to use
Talk to Thomas Honey. He is the Fortress rep, nice guy, and
knowledgeable wrench. He has stepped in on my issue.
Ray
On 11/16/2022 10:58 PM, Howie Michaelson via RE-wrenches wrote:
Good Evening,
I have a frustrating charging issue involving 2 Fortress eVault Maxs
connected to a Sol-Ark
e
aux out on the Classic to control a relay to turn on/off the inverters
for LVD, since Outback programming (like Schneider) won't allow LVD
settings above 48v.
Ray
On 11/16/2022 12:40 PM, Chris Sparadeo via RE-wrenches wrote:
Hi Ray,
I would suggest pushing the latest firmware update to
the batteries.
Has anyone else had a hard time with Fortress support? Does anyone have
a direct contact? Customer is beyond pissed now, after almost 2 weeks
hearing nothing, and having spent tens of thousands.
Thanks;
Ray Walters
Remote Solar
varied.
Ray Walters
On 9/30/2022 6:57 AM, Jay via RE-wrenches wrote:
Hi all and thanks for the input.
I guess he’s just been unlucky with the problems ( firmware upgrade
switching to 50hz) and possibly just some random bad hardware.
In regards to your thoughts of a install issue, he has spent
I agree with James here. I will relate a "funny" story about a neighbor
mounting a large Elk antler rack on his wall with lags. Worked fine,
till one night they heard a big crash, and the antlers had pulled the
wall stud right out of the wall into the living room. The 2x 4 came
right out of
Default efficiency on the TriMet was 94%, needs to be quite a bit higher
for Li+. I'd try 98%.
2nd point: Customers have always obsessed about meter readings: they
need to take a chill pill, and accept its not going to be better than
+/- 10% accuracy. Or get a Fortress battery with built
You'll use them for all sorts of stuff; good to keep on the truck.
Monk Wipes Heavy Duty Hand Cleaner | Large 9.6″ x 12 ...
Ray
Remote Solar
On 4/15/2022 8:56 AM, Garrison via RE-wrenches wrote:
Hi Mac,
I second the isopropyl alcohol (diluted), a soft cloth, and razor
blade if needed.
Mag
For disconnects, I'd just use Andersen quick connects. That's what they
use on forklifts and other industrial battery operated machines. Also,
the Magnum would act as the vehicle charger, and would be a much better
charger than the stock golf cart models.
Ray Walters
Remote Solar
303 505
Most carts run at 48vdc these days. They either have eight 6 volt
batteries, or six 8 v batteries. I would think that would make a good
match for power backup with a 4kw range inverter like the Magnum MS4448.
Ray
On 3/15/2022 12:18 PM, Nick A Lucchese wrote:
Not sure what the golf cart
The Midnite Classic can go higher to 72v stock, and they have models
that can work with 120 vdc batteries.
Ray
On 3/15/2022 12:19 PM, larrycrutcher wrote:
Hi William,
A charge controller may not be needed if you are running the pump
direct. By designing the PV array so that the Isc
PV System Disconnect, not RSS
Ray Walters
Remote Solar
303 505-8760
On 2/1/22 7:04 PM, Jeremy Rodriguez wrote:
Just a rated disco at the ground mount? Labeled as the rapid
shutdown switch?
That’s too simple!
In
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
transition point from the PV
system to all other systems, like battery or inverter systems. The
installer/ designer decides where to put that disconnect. I usually put
it on the wall before it goes into the building, and I have never had an
inspector question that.
Thanks,
Ray Walters
Remote
forgiving
though.
As for Milwaukee chucks jamming up; I only had that happen once after a
bunch of hammer drilling in Haiti. Scrounged all over the village for
the special star keys to take apart the chuck, but it just needed to be
cleaned.
Ray Walters
Remote Solar
303 505-8760
On 1/20/22
in the mountains.
Ray Walters
Remote Solar
303 505-8760
On 1/18/22 9:17 AM, Tump wrote:
Ray I would love to know which larger propane gen set you are
suggesting. 1800 or 3600 rpm. Air cooled or water cooled. To my
knowledge there are very few L cooled 1800 rpm gen sets in the 12-15kW
range. T
On Jan 17
consumption at the proposed load.
Plus the larger gensets are usually built to last longer than the
portable stuff.
Ray Walters
Remote Solar
303 505-8760
On 1/17/22 5:33 PM, Jeff Clearwater wrote:
Hello Again All,
Or I'd consider suggesting propane to the customer as well. Any
experience
That's a long enough run that you really need to weigh the cost of a
separate system. I'm not seeing the advantages of keeping a single
system for the whole island.
Ray Walters
Remote Solar
303 505-8760
On 1/10/22 9:43 AM, Chris Mason wrote:
I would use a 6,600V single phase outdoor pad
Long runs of URD direct buried? Just a nick into the metal can corrode
the cable all the way through over time. We use conduit for almost
everything anymore. The savings with URD doesn't pan out, when you have
to abandon the line after 10 years.
Ray Walters
Remote Solar
303 505-8760
On 1
AC coupled off grid? Sounds like a good time to go DC coupled.
Ray Walters
Remote Solar
303 505-8760
On 1/9/22 3:31 PM, Carl Adams wrote:
Mac,
SMA tech support told me this usually indicates a failing transformer
so as Marco suggests, the patient does not have long to live. I've
seen
All else fails, I just would go back to the Trace retail, give it a 10%
for being used, and call it good. $165? no one will complain about
that
On 12/10/2021 6:42 PM, Jerry Shafer wrote:
Truely it depends, if someone is looking and needing that part, the
sky is the limit, its its
, their
regular breakers are 150 vdc rated. I only use the 300 v rated breakers
with the new FM 100 that can take 300 vdc.
Ray Walters
Remote Solar
On 10/25/2021 6:45 PM, Chris Sparadeo wrote:
Hi Jeremy,
According to the QO cut sheet the answer is 48VDC:
https://download.schneider-electric.com/files
Is this something else we need to put into our contracts?
"Not responsible for sounds due to normal thermal expansion and
contraction of racking, modules, and roof".
Ray Walters
Remote Solar
On 10/20/2021 2:58 PM, Jason Szumlanski wrote:
These were Black framed Axitec panels.
ave not tried in cold weather, is diesels. I have
clients in warmer places with Kubotas that have offered excellent
service. I have clients in Alaska that love their diesels, but I'm not
sure what they've done to cold proof them.
Ray Walters
Remote Solar
On 10/19/2021 1:13 PM, Sindelar Solar wr
,
the screws can start binding from over heating, if driven too fast.
Ray Walters
Remote Solar
303 505-8760
On 9/4/21 12:08 PM, Jerry Shafer wrote:
Wrenches
its not the tool its the user so when I hear about impacts got to know
the feel.
Jerry
On Fri, Sep 3, 2021 at 12:06 AM Corey Shalanski
level RSD is not.
Ray Walters
Remote Solar
303 505-8760
On 8/28/21 9:46 AM, Dave Angelini Offgrid Solar wrote:
The Schneider RSD is decent. At least it is useable as a 600vdc disco.
Wink The few offgrid homes that were required to use this had the Tigo
units on the array panels and wireless
an indoor rated
connection only to me.
Ray Walters
Remote Solar
303 505-8760
On 8/16/21 12:54 PM, AE Solar wrote:
Wrenchers,
Some point back we transitioned from polaris lugs to buchanan
crimps/caps (doping our wires in noalox) for our jbox splices. I know
there have been a few conversations
much earlier and get much
more water over the day. Its also easier on a low flow well to pump a
little bit through out the day, than have a big pump hit it hard a few
times a day.
Ray Walters
Remote Solar
303 505-8760
On 7/26/21 10:02 PM, Mac Lewis wrote:
Hi Howie,
There are many options
system?
Ray Walters
Remote Solar
303 505-8760
On 7/26/21 7:15 PM, Dana Orzel wrote:
Hey all!
I am proposing a [20] module, 35˚ tilt up array mounted on a flat roof
in snow country - Central Idaho. Its in town, trees behind & off to
the side a ways.
The SnapnRack design calls for
Hi Jeremy;
Based on the age, and brand, I'd say its time for new batteries. Steve's
comments, as always, are great information. From my experience, L16s
are fairly unpredictable, and you could start seeing cell failures this
next cold season.
Ray Walters
Remote Solar
303 505-8760
On 7/21
again, I don't know. It might be better than steel, but
all are allowed by code.
Ultimately it might come down to soil and weather conditions for
different areas?
Ray Walters
Remote Solar
303 505-8760
On 6/25/21 10:35 AM, Dana Orzel wrote:
That’s why we use the Ufer, our AHJ assumes that
We always put our assumption in our plan notes, based on our
interpretation of 250.52(A)(7). AHJs have never questioned it, and we
also tie the pole to any rebar, so its all one big happy grounding
electrode.
Ray Walters
Remote Solar
303 505-8760
On 6/24/21 6:49 PM, frenergy wrote:
Ray
Usually a steel pole in concrete has enough surface area to qualify as a
plate electrode under 250.52(A)(7). It needs to be at least 2 sq ft and
1/4" thick, and have an electrically conductive surface. So we just
drill and tap our ground connection into the pole, near the combiner box.
than the bolt itself. We've also done combinations, where we
can only get 18" of concrete over the rock, then we epoxy in rebar to
tie the concrete to the rock, and J bolts set in the concrete to bolt
the base plate to.
Ray Walters
Remote Solar
303 505-8760
On 6/23/21 7:01 PM, Dave Angeli
manus seem to have almost
zero desire to listen to wrenches and improve their designs.
Ray Walters
Remote Solar
303 505-8760
On 6/6/21 1:31 PM, la...@starlightsolar.com wrote:
The problem with Battle born heated battery is that it was an after
thought. It uses power from the battery to heat itself
Another shout out for the Trimetric folks. They revised the manuals
recently as well, nice job.
Ray Walters
Remote Solar
303 505-8760
On 6/4/21 1:13 PM, Sindelar Solar wrote:
Lou,
I spoke this morning with Kedar, who purchased Bogart Engineering
several years ago, about an out-of-warranty
HUPs can be wired end to end to fit pretty close to that space.
Ray Walters
Remote Solar
303 505-8760
On 5/29/21 12:50 PM, palumbo1...@gmail.com wrote:
Our old Surrette Rolls distributor, RAE Storage Battery, has been sold
to another battery manufacturer and they no longer sell Surrette
they made a 48v pack.
https://www.lifebluebattery.com/rv-boat-low-temperature-lithium-ion-batteries/index.html
Ray Walters
Remote Solar
303 505-8760
On 5/21/21 12:12 PM, Larry wrote:
My personal opinion is that you should not buy any lithium battery that does
not provide adequate protection
or large loads in the backup.
Ray Walters
Remote Solar
303 505-8760
On 5/20/21 12:26 PM, palumbo1...@gmail.com wrote:
I’m going to be upgrading on old dual inverter OutBack FX 2524 system
to dual VFX3524 inverters and would prefer to not use the new R series
as I have heard about problems
Thanks Dan, that has also been my understanding of all listed
equipment. Certain switches etc will say on them "AC only", or give
different DC ratings. Otherwise the voltage listing is AC/DC.
Ray Walters
Remote Solar
303 505-8760
On 5/10/21 2:55 PM, Dan Fink wrote:
Esteemed W
check that William mentioned. Has anybody tried them?
https://www.phoenixcontact.com/online/portal/us?1dmy=wcm%3apath%3a/usen/web/main/products/subcategory_pages/Modular_terminal_blocks_for_photovoltaics_P-15-09/eb8c193d-6a2d-4349-8f89-2d523fd5b04f
Ray Walters
Remote Solar
303 505-8760
On 5/7/21 8
on my cell service. Think about what this biz would be
like without this form, and then support it accordingly. Biz has been
good, don't be a chump!
Rant off, Thanks Michael.
Ray Walters
Remote Solar
303 505-8760
On 5/5/21 9:01 PM, drake.chamber...@redwoodalliance.org wrote:
Hello Wrench
I second that.
Ray Walters
Remote Solar
303 505-8760
On 5/6/21 10:33 AM, Dave Angelini Offgrid Solar wrote:
I would not do any of this for an offgrid client. It is against the
rule of less is more. The whole design is flawed in my opinion.
*Dave Angelini Offgrid Solar "we go
Hi Glenn;
Ahh that's new from NEC 2014. Thanks for pointing that out, and scratch
my previous comment based on experiences in 2008.
Ray Walters
Remote Solar
303 505-8760
On 4/29/21 11:41 AM, Glenn Burt wrote:
NEC 314.15 discusses drainage openings that can be made in enclosures
might not like it.
Ray Walters
Remote Solar
303 505-8760
On 4/29/21 9:43 AM, frenergy wrote:
Eric,
I like your idea of drilling the weepage holes as long as
they are not big enough to allow critters like wasps to make a home
inside the J-box. We will use aluminum tape on unused
the manufacturer's retest to 1000v. I can't imagine those
blocks not being able to handle 1000v, but.
Ray Walters
Remote Solar
303 505-8760
On 4/28/21 11:27 AM, Corey Shalanski wrote:
Chris's reminder is a good one—the 600V rating of most insulated
"multi-tap" connectors pretty much limits
, if not
really done well.
Ray Walters
Remote Solar
303 505-8760
On 4/26/21 11:16 PM, frenergy wrote:
Blake,
Its great to get definitive clarification on this MC4/THHN
issue, we've been using 4-14 Polaris connectors with good results.
Being inside a Nema3 can and having silicone grease
to prioritize the house battery.
Ray Walters
Remote Solar
303 505-8760
On 4/13/21 4:29 PM, la...@starlightsolar.com wrote:
Mac,
You can charge with DC directly from a PV solar array without an
inverter or regulator. The current is self limiting by the amount of
PV solar power you are making at any
it was so
out of the ordinary. How about a #4 ground wire that looks properly
attached at the electrode and back at the main AC panel, but turned out
to be not connected in the wall.in a J box that had been plastered over.
Ray Walters
Remote Solar
303 505-8760
On 3/31/21 12:48 PM, William
ting surge.
Or you could go 21st century, with 48v, Li+ PWM controller, etc
Another option to consider is using existing Li+ battery packs, like
Ryobi's 40 v lawn mower packs.
Ray Walters
Remote Solar
303 505-8760
On 3/26/21 5:32 PM, Dana Orzel wrote:
Hey All wise ones,
I have an
How big is the battery bank? How old is it? It doesn't look that far
off of what I've seen in GTB systems.
Ray Walters
Remote Solar
303 505-8760
On 3/19/21 12:21 PM, Christopher Warfel wrote:
I have not been able to find a way to set my customers battery
charging parameters so that the AGM
1 - 100 of 1180 matches
Mail list logo