Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Ray Walters via RE-wrenches
enough air.   You didn't mention gen set model, or whether the frequency was a solid 60 hz.  I've seen bad things happen when the frequency got out of spec too.  I'm guessing a bad voltage regulator on the gen set. Ray Walters Remote Solar On 4/25/2024 11:24 AM, Kevin Pegg via RE-wrenches wrote

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Ray Walters via RE-wrenches
.  The cheapo BMS lears its ugly head once again.  All we're doing lately is fixing stuff less than 5 years old. Ray Walters Remote Solar On 4/25/2024 9:52 AM, Michael Morningstar via RE-wrenches wrote: Here's a different take. Just food for thought and not necessarily a suggestion. Those 1st

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Ray Walters via RE-wrenches
and the customer can be bored for a decade.  It will make more power too, especially on cold, sunny days when you really need it. Ray Walters Remote Solar On 4/23/2024 12:47 PM, Todd Cory via RE-wrenches wrote: My old MX60 said " hot" when the fan had failed. Todd "MX 2 Hot (Very rare)

Re: [RE-wrenches] Plaques

2024-03-30 Thread Ray Walters via RE-wrenches
it in house to pencil out. I'm not sure if it ever would, considering that you still have to pay yourself or someone else to operate the engraver, and the blank plaques probably cost a bit too. Ray Walters Remote Solar On 3/30/2024 12:56 PM, Lou Russo via RE-wrenches wrote: Aloha Wrenches, Anyone

Re: [RE-wrenches] Minimum bus size, new requirements

2024-03-28 Thread Ray Walters via RE-wrenches
applications.   The rest of us in the other 49 states are Not required to comply with the 200 A requirement. Good Luck out there. Thank you, Ray Walters Remote Solar On 3/28/2024 12:33 PM, Lloyd Hoffstatter via RE-wrenches wrote: William, Here is the CA Energy Code with the upsized busbar

Re: [RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?

2024-03-13 Thread Ray Walters via RE-wrenches
xception 1 specifically says a single N-G bond is allowed for multiple power sources. Ray Walters Remote Solar On 3/13/2024 3:19 PM, Mick Abraham via RE-wrenches wrote: Hi, Mechanix~ My off grid project gig has redundant 120y208 generators that need a 200a "break before make" manua

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Ray Walters via RE-wrenches
for, and I sleep well at night with my standard contractor's liability insurance. Remember, insurance agents primary goal is to sell more insurance.  Of course they want you to have an E policy, too. Ray Walters Remote Solar On 3/11/2024 7:41 PM, Howie Michaelson via RE-wrenches wrote: William, et

Re: [RE-wrenches] TPM Search

2024-03-10 Thread Ray Walters via RE-wrenches
down mounting, and no losses.   I've been  suspicious of top down module racking; and I was quite satisfied with actual bolts and hardware to hold modules in place.  But its just not true anymore.    I added 3/4" angle stainless steel to reinforce the attachments on the top modules. Ray Walters On

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
Here's another mount at the edge of failure, from the same system. Hardware is tight.  Like many, I had lots of love for good ol' fashion bottom mounting vs top mount, until this happened about 5 years ago. This is how we learn. On 3/8/2024 5:15 PM, Ray Walters via RE-wrenches wrote: I've

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
I've had several modules pull off of bottom mount racking in high winds, but never top mount racking.  Newer modules have much thinner frames, but are much more surface area than the old days. So to answer Kent's question: Ray Walters Remote Solar On 3/8/2024 3:50 PM, Kent via RE-wrenches

Re: [RE-wrenches] Battery Electrolyte Level Measuring

2024-02-29 Thread Ray Walters via RE-wrenches
that's quite accurate; I tried it on some bottles with fluid in them, and it seemed to work well.  I'll try and remember to take out with me on the next job with FLA. Ray Walters Remote Solar On 2/29/2024 2:12 PM, William Miller via RE-wrenches wrote: Friends: Thanks to everyone who responded

Re: [RE-wrenches] Rugged Wind/Solar System For Radio

2024-02-21 Thread Ray Walters via RE-wrenches
Who carries the Superwind turbines?  We've been looking for a replacement for the old Bergey XL1 to offer clients. Thanks, Ray Walters Remote Solar On 2/21/2024 7:20 PM, John Blittersdorf via RE-wrenches wrote: As far as wind is concerned, I recommend SuperWind, made in Germany.  It is well

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
like "lead acid batteries aren't allowed", will get them to back down on the spot.  Getting solar trade organizations on your side to help with the process can add much needed weight. Ray Walters Remote Solar On 2/17/2024 2:26 PM, Dan Fink via RE-wrenches wrote: Jay - Despite the excepti

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
ere. Also, with all the mention of various UL listings, regulation needs to evolve to differentiate between LiFePO4 and other Li+ chemistries.  LiFePO4 is inherently much safer, but we're being forced to comply with all the same regulations as the less stable, more energy dense chemistries. R

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work

Re: [RE-wrenches] XW EQ question

2024-02-12 Thread Ray Walters via RE-wrenches
What's funny, is the good old SWs from the Trace days had the same problem.   Never could get them to equalize.  Maybe that software carried over. Ray Walters Remote Solar On 2/12/2024 4:42 PM, jay via RE-wrenches wrote: Hi Kevin Thanks, I heard that exact thing from someone else. Do you

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
Hi Richard; Off list, what was your outcome from Simpliphi?  Did they make any deal with you?  What did you put in as replacements? Thanks, Ray Walters Remote Solar On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote: Hi Ray We had a complete failure of 6 Simpliphi batteries

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
ng for SLA batteries to get this customer back in action. Reporting as always from the Bleeding Edge, Ray Walters Remote Solar On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote: Hi Ray We had a complete failure of 6 Simpliphi batteries with the same symptoms you found. Another ins

Re: [RE-wrenches] Lithium batteries

2024-02-07 Thread Ray Walters via RE-wrenches
of these high price tag batteries don't start failing on my watch. I've been holding this rant back for a while, trying to give Simpliphi a chance to make this right. However, this week I heard their "diagnosis", and then I saw Jay's timely post? I knew it was time.  Sincerely, R

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
I'm trying to find a pic to post, but they were MC4 connectors, not the UTX. Ray On 11/9/2023 4:57 PM, Brian Mehalic wrote: Are they the Amohenol UTX connectors? SW had a recall on them, sounds like about the right timeframe. BREAKING: SolarWorld recalls PV modules with Amphenol connectors

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
connector type. 10+ amps continuous, moist environment, 30F+  hotter than ambient temp, all are tough on connectors.  I predict more connector failures as module current ratings increase. Ray Walters Remote Solar On 11/9/2023 3:02 PM, Glenn Burt via RE-wrenches wrote: Good luck trying to con

Re: [RE-wrenches] Need a hand with Sunny Island/Sunny boy AC couple

2023-10-21 Thread Ray Walters via RE-wrenches
What is the array size vs the battery size?  Sounds like a big array on a small battery for the voltage to go that high that fast. Ray Remote Solar On 10/21/2023 5:46 PM, William Miller via RE-wrenches wrote: Friends: I’m kinda stuck on a project setting up a SI/SB AC coupled system off

Re: [RE-wrenches] Power conditioner for Trace inverter

2023-09-08 Thread Ray via RE-wrenches
s?  Definitely needs to be in a metal enclosure. I think its either get a different washer or get a different inverter. At 22+ years, its slowly reaching the time to retire those old SWs. Ray Walters Remote Solar 303 505-8760 On 9/8/23 2:53 PM, Dave Angelini Offgrid Solar via RE-wrenches wrot

Re: [RE-wrenches] Wind machines

2023-08-17 Thread Ray Walters via RE-wrenches
, which is what many folks find attractive, I think. Ray Walters On 8/17/2023 1:41 PM, Jay via RE-wrenches wrote: Im curious if anyone has actual measured data on a VAWT. It just seems like they are meat for the end of the worlders Jay ___ List

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
manually turn the inverters back on. Ray On 7/20/2023 5:15 PM, Jay wrote: Hi Ray This house won’t have an AGS, manual start only. And your comments exactly, having to wait until the next day when hopefully there is enough sun to charge the battery is iffy. Or they could do the inverter bypass

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
The aux off is only if the generator doesn't start.  You need to set the gen start voltage higher. Aux off is last ditch shut down, set for 44v for lead acid, or 47 to 49v, depending on the battery and inverter.   Hopefully DC coupled PV will raise the voltage enough to turn the inverters back

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread Ray Walters via RE-wrenches
brand BTW. Ray Walters On 7/16/2023 4:18 PM, Kent via RE-wrenches wrote: I think these modules are about 12 years old. I didn't have a voltmeter or ammeter with me this morning when this was discovered so I wasn't able to check the output. Kent Osterberg Blue Mountain Solar On 7/16/2023 3:06

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-13 Thread Ray Walters via RE-wrenches
. Absolutely makes no sense.  Schneider, Outback, even Magnum is too low...? Ray Walters On 7/11/2023 6:19 PM, Mac Lewis via RE-wrenches wrote: Hello Wrenches, I'm trying to solve an issue with an older Outback FX system.  It's a quad stack of Outback 3648 FX inverters and he has a couple

Re: [RE-wrenches] Inverter output fluctuations

2023-07-03 Thread Ray Walters via RE-wrenches
of the driver circuits on the LED bulbs.  Only gets worse on a less than perfect AC waveform. Ray Walters Remote Solar On 7/3/2023 5:09 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote: I think I would try eliminating things. Turn off the AC coupling for a few days and get results. Turn

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
.  That sounds more like a cooked control board.  I had lightning damage cause an inverter to put out 140 vac, while its onboard electronics read 120 vac. If it helps, I have a used MS 4024 PAE (very low hours) that I could send to you.   Contact me off list if you want. Ray Walters Remote Solar

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
g off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power outp

Re: [RE-wrenches] Metering

2023-05-11 Thread Ray Walters via RE-wrenches
production on the PV system, and then do some subtraction.  Pretty simple for them, and you only get a call, if the inverter production is low or off. Ray Walters Remote Solar On 5/11/2023 2:20 PM, Larry Brown via RE-wrenches wrote: Does anyone have a recommendation for a high quality meter

Re: [RE-wrenches] Solar direct water pumping

2023-05-08 Thread Ray Walters via RE-wrenches
looked up (just like wire losses) for the size pipe and flow rate. Finally, you didn't mention how large a pond.  To fill the pond, it needs to overcome both evaporative losses, and leakage into the surrounding soil. Ray Walters Remote Solar On 5/8/2023 10:04 AM, Howie Michaelson via RE-wren

Re: [RE-wrenches] Truss finder

2023-04-17 Thread Ray Walters via RE-wrenches
If the temperature is right, my IR camera can see the rafters. Best to check early on a cold morning with the heat on in the building.  Otherwise I'm of the William "Hammer" system persuasion.  Never found anything better. On 4/17/2023 1:31 PM, Garrison via RE-wrenches wrote: Hi Kris, I

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
on't cheap out. Ray Walters Remote Solar On 4/4/2023 5:42 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote: Hurts my head !  Agree that you will have more trips to this house after the next one. This is most likely not going to get you 2 more years. All of the wiring is good, clean, and t

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
the inverters.  IF the inverters are Outback, they have a remote switch, if its something else, you might have to actually switch off a relay on the AC output. Ray On 4/4/2023 2:45 PM, Daniel Young via RE-wrenches wrote: Thanks all for the advice. I figured it was not worth trying on a different battery

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread Ray Walters via RE-wrenches
, I've seen less than 5 years from sealed L16s like Trojan.  Full River is about the best in that field, and still only going to see 7 to 8 years.  It just doesn't pencil out compared to HUPs or Li+. Ray Walters Remote Solar On 4/3/2023 12:39 PM, William Miller via RE-wrenches wrote: Daniel: I

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-31 Thread Ray Walters via RE-wrenches
a bit better with new found idea on each install. Thanks again for great ideas Wrenches, Ray On 3/31/2023 2:15 PM, Jason Szumlanski wrote: Hi Ray, I'm happy to have some confirmation from another major storm's impact. My father has a home in Dominica, which was hit by Maria with 165 mph winds

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-30 Thread Ray Walters via RE-wrenches
Use an electric screw driver, socket wrench, or *drill with a clutch* set low to snug up the clamps, and then final torque with a torque wrench. Period. Ray Walters Remote Solar Former NABCEP 2004-2016 On 3/30/2023 4:34 PM, Jason Szumlanski via RE-wrenches wrote: That would be great if it were pos

Re: [RE-wrenches] Off Grid Battery Charging

2023-03-16 Thread Ray Walters via RE-wrenches
th wiring into the system.  Maybe she could do what several folks have done: power a TV while you pedal.  Anyway, here is device that might do it:   https://www.econvergence.net/ Ray Walters Remote Solar On 3/16/2023 3:58 PM, Larry Brown via RE-wrenches wrote: Wrenches I have a client that we did a

[RE-wrenches] Fire Sprinklers (was Re: Cell phone based relay control)

2023-03-14 Thread Ray Walters via RE-wrenches
a couple pics of your sprayer install? 2nd question:  what are the field results of these systems in actual fires? Thanks, Ray On 3/14/2023 10:03 AM, Todd Cory via RE-wrenches wrote: I can help with this as Michael built something similar to what I designed and installed in 2001: I plumbed

Re: [RE-wrenches] Cell phone based relay control

2023-03-13 Thread Ray Walters via RE-wrenches
Michael; Can you share more about your sprinkler system and the power supply for it?  Over the years, at least two of my customers have lost their homes (and PV arrays) in wild fires. Ray Walters Remote Solar On 3/13/2023 2:34 PM, Michael Morningstar via RE-wrenches wrote: WebRelay. I use

Re: [RE-wrenches] PV and EMP

2023-03-09 Thread Ray Walters via RE-wrenches
I'm not an EMP expert by any means, but I've dealt with quite a few lightning damaged systems.  Having a good connection to a low impedance grounding system (steel cased well, Ufer ground) is crucial.  I also have had fantastic luck with Midnite's MNSPD line.  Delta, not so much. On 3/9/2023

[RE-wrenches] 60v Inverter?

2023-03-02 Thread Ray Walters via RE-wrenches
that is in an Hammond organ, so that I can tune the organ down from A=440 Hz to A =432 Hz to match an even older piano.Yep, I'm living on the edge.. Ray Walters (Now Even More) Remote Solar ___ List sponsored by Redwood Alliance Pay optional

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
for anything greater than 60 amps for 2 poles, other than large DPDT switches which get pricey and hard to source especially for 200 amps? Howie On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches wrote: I probably still have one of the old QO boxes on the shelf, but I never liked

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
://www.northerntool.com/shop/tools/product_200653609_200653609 Midnite makes small 30A and 60A T switches as well: https://www.midnitesolar.com/productPhoto.php?product_ID=416_ID=29=3=p Ray Walters On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote: Kris, It was SqD QO403, and it was a 3-pole load center

[RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Ray Walters via RE-wrenches
than squeezing an extra 5% capacity out of the battery Notes in the online instructions such as "/Failure to properly upgrade the firmware may cause the battery to stop working!", / are not making we want to push ahead with closed loop either. Ray On 2/9/2023 11:01 AM, Chris Sc

[RE-wrenches] Fortress Battery Heater

2023-02-08 Thread Ray Walters via RE-wrenches
with the Solark's load controls. I've considered some DC options, but they don't make much sense, since the inverter has to be on to charge from PV anyway. The long term plan is for the client to finish the insulation, and sheet rock, and add a gas wall heater in there as needed. Thanks, Ray Walters

Re: [RE-wrenches] Magnum MS4024 grief

2022-12-16 Thread Ray Walters via RE-wrenches
bunch of DIY garbage.  Find out who did the original wiring.  Probably not a pro. Ray Walters Remote Solar On 12/16/2022 11:35 AM, Kirk Herander via RE-wrenches wrote: You may have neutral and ground connected at more than 1 location, meaning at the genset and in house panel, which means the ground

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Ray Walters via RE-wrenches
To add to Jeff's suggestion of targeting 95%, many Li+ batteries have a spike in voltage as they reach 100%.  We just don't have to worry anymore about sulfate damage from under charging. Ray Walters Remote Solar On 11/19/2022 7:14 AM, Jeff Clearwater via RE-wrenches wrote: Hi Kris What

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-17 Thread Ray Walters via RE-wrenches
, with built in color touch screen for monitoring, price much better. Simpliphi = no monitoring at all, have to parallel ridiculous qty of batteries to do a normal off grid home, but integration guides are the best. Ray Walters On 11/17/2022 1:16 PM, r...@solartechvt.com wrote: We’ve started to use

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-16 Thread Ray Walters via RE-wrenches
Talk to Thomas Honey.  He is the Fortress rep, nice guy, and knowledgeable wrench.   He has stepped in on my issue. Ray On 11/16/2022 10:58 PM, Howie Michaelson via RE-wrenches wrote: Good Evening, I have a frustrating charging issue involving 2 Fortress eVault Maxs connected to a Sol-Ark

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
e aux out on the Classic to control a relay to turn on/off the inverters for LVD, since Outback programming (like Schneider) won't allow LVD settings above 48v. Ray On 11/16/2022 12:40 PM, Chris Sparadeo via RE-wrenches wrote: Hi Ray, I would suggest pushing the latest firmware update to

[RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
the batteries. Has anyone else had a hard time with Fortress support?  Does anyone have a direct contact?  Customer is beyond pissed now, after almost 2 weeks hearing nothing, and having spent tens of thousands. Thanks; Ray Walters Remote Solar

Re: [RE-wrenches] sol ark reliability question

2022-09-30 Thread Ray Walters via RE-wrenches
varied. Ray Walters On 9/30/2022 6:57 AM, Jay via RE-wrenches wrote: Hi all and thanks for the input. I guess he’s just been unlucky with the problems ( firmware upgrade switching to 50hz) and possibly just some random bad hardware. In regards to your thoughts of a install issue, he has spent

Re: [RE-wrenches] Discover AES Wall Mount Considerations

2022-09-06 Thread Ray Walters via RE-wrenches
I agree with James here.  I will relate a "funny" story about a neighbor mounting a large Elk antler rack on his wall with lags. Worked fine, till one night they heard a big crash, and the antlers had pulled the wall stud right out of the wall into the living room. The 2x 4 came right out of 

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Ray Walters via RE-wrenches
Default efficiency on the TriMet was 94%, needs to be quite a bit higher for Li+.  I'd try 98%. 2nd point:  Customers have always obsessed about meter readings: they need to take a chill pill, and accept its not going to be better than +/- 10% accuracy.  Or get a Fortress battery with built

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Ray Walters via RE-wrenches
You'll use them for all sorts of stuff; good to keep on the truck. Monk Wipes Heavy Duty Hand Cleaner | Large 9.6″ x 12 ... Ray Remote Solar On 4/15/2022 8:56 AM, Garrison via RE-wrenches wrote: Hi Mac, I second the isopropyl alcohol (diluted), a soft cloth, and razor blade if needed. Mag

Re: [RE-wrenches] Golf Cart as temporary off-grid PV

2022-03-16 Thread Ray
For disconnects, I'd just use Andersen quick connects.  That's what they use on forklifts and other industrial battery operated machines.  Also, the Magnum would act as the vehicle charger, and would be a much better charger than the stock golf cart models. Ray Walters Remote Solar 303 505

Re: [RE-wrenches] Golf Cart as temporary off-grid PV

2022-03-15 Thread Ray Walters
Most carts run at 48vdc these days.  They either have eight 6 volt batteries, or six 8 v batteries.  I would think that would make a good match for power backup with a 4kw range inverter like the Magnum MS4448. Ray On 3/15/2022 12:18 PM, Nick A Lucchese wrote: Not sure what the golf cart

Re: [RE-wrenches] 24/7 Water pumping

2022-03-15 Thread Ray Walters
The Midnite Classic can go higher to 72v stock, and they have models that can work with 120 vdc batteries. Ray On 3/15/2022 12:19 PM, larrycrutcher wrote: Hi William, A charge controller may not be needed if you are running the pump direct. By designing the PV array so that the Isc

Re: [RE-wrenches] Rapid Shutdown for Off-grid systems

2022-02-01 Thread Ray
PV System Disconnect, not RSS Ray Walters Remote Solar 303 505-8760 On 2/1/22 7:04 PM, Jeremy Rodriguez wrote: Just a rated disco at the ground mount?   Labeled as the rapid shutdown switch? That’s  too simple! In Jeremy Rodriguez Solar Installation / Design Expert All Solar, Inc. 1453 M St

Re: [RE-wrenches] Rapid Shutdown for Off-grid systems

2022-02-01 Thread Ray
transition point from the PV system to all other systems, like battery or inverter systems. The installer/ designer decides where to put that disconnect.  I usually put it on the wall before it goes into the building, and I have never had an inspector question that. Thanks, Ray Walters Remote

Re: [RE-wrenches] Lithium Ion tool batteries

2022-01-20 Thread Ray
forgiving though. As for Milwaukee chucks jamming up;  I only had that happen once after a bunch of hammer drilling in Haiti.  Scrounged all over the village for the special star keys to take apart the chuck, but it just needed to be cleaned. Ray Walters Remote Solar 303 505-8760 On 1/20/22

Re: [RE-wrenches] Conext XW Pro Compatible Generators?

2022-01-18 Thread Ray
in the mountains. Ray Walters Remote Solar 303 505-8760 On 1/18/22 9:17 AM, Tump wrote: Ray I would love to know which larger propane gen set you are suggesting. 1800 or 3600 rpm. Air cooled or water cooled.  To my knowledge there are very few L cooled 1800 rpm gen sets in the 12-15kW range. T On Jan 17

Re: [RE-wrenches] Conext XW Pro Compatible Generators?

2022-01-17 Thread Ray
consumption at the proposed load. Plus the larger gensets are usually built to last longer than the portable stuff. Ray Walters Remote Solar 303 505-8760 On 1/17/22 5:33 PM, Jeff Clearwater wrote: Hello Again All, Or I'd consider suggesting propane to the customer as well.  Any experience

Re: [RE-wrenches] Transmitting 15kW 3600ft Off Grid.

2022-01-10 Thread Ray
That's a long enough run that you really need to weigh the cost of a separate system.  I'm not seeing the advantages of keeping a single system for the whole island. Ray Walters Remote Solar 303 505-8760 On 1/10/22 9:43 AM, Chris Mason wrote: I would use a 6,600V single phase outdoor pad

Re: [RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Ray
Long runs of URD direct buried?  Just a nick into the metal can corrode the cable all the way through over time.  We use conduit for almost everything anymore.  The savings with URD doesn't pan out, when you have to abandon the line after 10 years. Ray Walters Remote Solar 303 505-8760 On 1

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Ray
AC coupled off grid?  Sounds like a good time to go DC coupled. Ray Walters Remote Solar 303 505-8760 On 1/9/22 3:31 PM, Carl Adams wrote: Mac, SMA tech support told me this usually indicates a failing transformer so as Marco suggests, the patient does not have long to live.  I've seen

Re: [RE-wrenches] Fair price for an obsolete component

2021-12-10 Thread Ray Walters
All else fails, I just would go back to the Trace retail, give it a 10% for being used, and call it good.   $165?    no one will complain about that On 12/10/2021 6:42 PM, Jerry Shafer wrote: Truely it depends, if someone is looking and needing that part, the sky is the limit, its its

Re: [RE-wrenches] DC Rating of Square D QO?

2021-10-25 Thread Ray Walters
, their regular breakers are 150 vdc rated. I only use the 300 v rated breakers with the new FM 100 that can take 300 vdc. Ray Walters Remote Solar On 10/25/2021 6:45 PM, Chris Sparadeo wrote: Hi Jeremy, According to the QO cut sheet the answer is 48VDC: https://download.schneider-electric.com/files

Re: [RE-wrenches] Strange noises from the roof

2021-10-20 Thread Ray Walters
Is this something else we need to put into our contracts? "Not responsible for sounds due to normal thermal expansion and contraction of racking, modules, and roof". Ray Walters Remote Solar On 10/20/2021 2:58 PM, Jason Szumlanski wrote: These were Black framed Axitec panels.

Re: [RE-wrenches] Generator recommendation request

2021-10-19 Thread Ray Walters
ave not tried in cold weather, is diesels.  I have clients in warmer places with Kubotas that have offered excellent service.  I have clients in Alaska that love their diesels, but I'm not sure what they've done to cold proof them. Ray Walters Remote Solar On 10/19/2021 1:13 PM, Sindelar Solar wr

Re: [RE-wrenches] Over-torquing Module Clamps?

2021-09-04 Thread Ray
, the screws can start binding from over heating, if driven too fast. Ray Walters Remote Solar 303 505-8760 On 9/4/21 12:08 PM, Jerry Shafer wrote: Wrenches its not the tool its the user so when I hear about impacts got to know the feel. Jerry On Fri, Sep 3, 2021 at 12:06 AM Corey Shalanski

Re: [RE-wrenches] Exploding RSD Unit

2021-08-28 Thread Ray
level RSD is not. Ray Walters Remote Solar 303 505-8760 On 8/28/21 9:46 AM, Dave Angelini Offgrid Solar wrote: The Schneider RSD is decent. At least it is useable as a 600vdc disco. Wink The few offgrid homes that were required to use this had the Tigo units on the array panels and wireless

Re: [RE-wrenches] Buchanan Crimps in Outdoor Boxes

2021-08-16 Thread Ray
an indoor rated connection only to me. Ray Walters Remote Solar 303 505-8760 On 8/16/21 12:54 PM, AE Solar wrote: Wrenchers, Some point back we transitioned from polaris lugs to buchanan crimps/caps (doping our wires in noalox) for our jbox splices. I know there have been a few conversations

Re: [RE-wrenches] Remote AC well pump

2021-07-26 Thread Ray
much earlier and get much more water over the day.  Its also easier on a low flow well to pump a little bit through out the day, than have a big pump hit it hard a few times a day. Ray Walters Remote Solar 303 505-8760 On 7/26/21 10:02 PM, Mac Lewis wrote: Hi Howie, There are many options

Re: [RE-wrenches] Lighter tubing?

2021-07-26 Thread Ray
system? Ray Walters Remote Solar 303 505-8760 On 7/26/21 7:15 PM, Dana Orzel wrote: Hey all! I am proposing a [20] module, 35˚ tilt up array mounted on a flat roof in snow country - Central Idaho. Its in town, trees behind & off to the side a ways. The SnapnRack design calls for

Re: [RE-wrenches] High to normal SG

2021-07-21 Thread Ray
Hi Jeremy; Based on the age, and brand, I'd say its time for new batteries. Steve's comments, as always, are great information.  From my experience, L16s are fairly unpredictable, and you could start seeing cell failures this next cold season. Ray Walters Remote Solar 303 505-8760 On 7/21

Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

2021-06-25 Thread Ray
again, I don't know. It might be better than steel, but all are allowed by code. Ultimately it might come down to soil and weather conditions for different areas? Ray Walters Remote Solar 303 505-8760 On 6/25/21 10:35 AM, Dana Orzel wrote: That’s why we use the Ufer, our AHJ assumes that

Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

2021-06-24 Thread Ray
We always put our assumption in our plan notes, based on our interpretation of 250.52(A)(7).  AHJs have never questioned it, and we also tie the pole to any rebar, so its all one big happy grounding electrode. Ray Walters Remote Solar 303 505-8760 On 6/24/21 6:49 PM, frenergy wrote: Ray

Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

2021-06-24 Thread Ray
Usually a steel pole in concrete has enough surface area to qualify as a plate electrode under 250.52(A)(7).  It needs to be at least 2 sq ft and 1/4" thick, and have an electrically conductive surface.  So we just drill and tap our ground connection into the pole, near the combiner box.

Re: [RE-wrenches] Top of Pole Mount Array on Ledge

2021-06-23 Thread Ray
than the bolt itself.  We've also done combinations, where we can only get 18" of concrete over the rock, then we epoxy in rebar to tie the concrete to the rock, and J bolts set in the concrete to bolt the base plate to. Ray Walters Remote Solar 303 505-8760 On 6/23/21 7:01 PM, Dave Angeli

Re: [RE-wrenches] LiFePo4 Low Temp Charging Damage

2021-06-06 Thread Ray
manus seem to have almost zero desire to listen to wrenches and improve their designs. Ray Walters Remote Solar 303 505-8760 On 6/6/21 1:31 PM, la...@starlightsolar.com wrote: The problem with Battle born heated battery is that it was an after thought. It uses power from the battery to heat itself

Re: [RE-wrenches] The Tri-Metric TM-2030-A and LFPs

2021-06-04 Thread Ray
Another shout out for  the Trimetric folks.  They revised the manuals recently as well, nice job. Ray Walters Remote Solar 303 505-8760 On 6/4/21 1:13 PM, Sindelar Solar wrote: Lou, I spoke this morning with Kedar, who purchased Bogart Engineering several years ago, about an out-of-warranty

Re: [RE-wrenches] Surrette Rolls distributors

2021-05-29 Thread Ray
HUPs can be wired end to end to fit pretty close to that space. Ray Walters Remote Solar 303 505-8760 On 5/29/21 12:50 PM, palumbo1...@gmail.com wrote: Our old Surrette Rolls distributor, RAE Storage Battery, has been sold to another battery manufacturer and they no longer sell Surrette

Re: [RE-wrenches] LiFePo4 Low Temp Charging Damage

2021-05-21 Thread Ray
they made a 48v pack. https://www.lifebluebattery.com/rv-boat-low-temperature-lithium-ion-batteries/index.html Ray Walters Remote Solar 303 505-8760 On 5/21/21 12:12 PM, Larry wrote: My personal opinion is that you should not buy any lithium battery that does not provide adequate protection

Re: [RE-wrenches] OB VFX3524M vs regular VFX

2021-05-20 Thread Ray
or large loads in the backup. Ray Walters Remote Solar 303 505-8760 On 5/20/21 12:26 PM, palumbo1...@gmail.com wrote: I’m going to be upgrading on old dual inverter OutBack FX 2524 system to dual VFX3524 inverters and would prefer to not use the new R series as I have heard about problems

Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-10 Thread Ray
Thanks Dan, that has also been my understanding of all listed equipment.  Certain switches etc will say on them "AC only", or give different DC ratings.  Otherwise the voltage listing is AC/DC. Ray Walters Remote Solar 303 505-8760 On 5/10/21 2:55 PM, Dan Fink wrote: Esteemed W

Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-08 Thread Ray
check that William mentioned.  Has anybody tried them? https://www.phoenixcontact.com/online/portal/us?1dmy=wcm%3apath%3a/usen/web/main/products/subcategory_pages/Modular_terminal_blocks_for_photovoltaics_P-15-09/eb8c193d-6a2d-4349-8f89-2d523fd5b04f Ray Walters Remote Solar 303 505-8760 On 5/7/21 8

Re: [RE-wrenches] Wrench Membership Dues

2021-05-06 Thread Ray
on my cell service. Think about what this biz would be like without this form, and then support it accordingly.  Biz has been good, don't be a chump! Rant off,  Thanks Michael. Ray Walters Remote Solar 303 505-8760 On 5/5/21 9:01 PM, drake.chamber...@redwoodalliance.org wrote: Hello Wrench

Re: [RE-wrenches] Generator and AC coupling on a Sol-Ark

2021-05-06 Thread Ray
I second that. Ray Walters Remote Solar 303 505-8760 On 5/6/21 10:33 AM, Dave Angelini Offgrid Solar wrote: I would not do any of this for an offgrid client. It is against the rule of less is more. The whole design is flawed in my opinion. *Dave Angelini Offgrid Solar "we go

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-29 Thread Ray
Hi Glenn; Ahh that's new from NEC 2014.  Thanks for pointing that out, and scratch my previous comment based on experiences in 2008. Ray Walters Remote Solar 303 505-8760 On 4/29/21 11:41 AM, Glenn Burt wrote: NEC 314.15 discusses drainage openings that can be made in enclosures

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-29 Thread Ray
might not like it. Ray Walters Remote Solar 303 505-8760 On 4/29/21 9:43 AM, frenergy wrote: Eric,             I like your idea of drilling the weepage holes as long as they are not big enough to allow critters like wasps to make a home inside the J-box.  We will use aluminum tape on unused

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-28 Thread Ray
the manufacturer's retest to 1000v.  I can't imagine those blocks not being able to handle 1000v, but. Ray Walters Remote Solar 303 505-8760 On 4/28/21 11:27 AM, Corey Shalanski wrote: Chris's reminder is a good one—the 600V rating of most insulated "multi-tap" connectors pretty much limits

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-27 Thread Ray
, if not really done well. Ray Walters Remote Solar 303 505-8760 On 4/26/21 11:16 PM, frenergy wrote: Blake,             Its great to get definitive clarification on this MC4/THHN issue, we've been using 4-14 Polaris connectors with good results.  Being inside a Nema3 can and having silicone grease

Re: [RE-wrenches] PV direct EV charging

2021-04-13 Thread Ray
to prioritize the house battery. Ray Walters Remote Solar 303 505-8760 On 4/13/21 4:29 PM, la...@starlightsolar.com wrote: Mac, You can charge with DC directly from a PV solar array without an inverter or regulator. The current is self limiting by the amount of PV solar power you are making at any

Re: [RE-wrenches] Odd inspection procedure

2021-03-31 Thread Ray
it was so out of the ordinary.  How about a #4 ground wire that looks properly attached at the electrode and back at the main AC panel, but turned out to be not connected in the wall.in a J box that had been plastered over. Ray Walters Remote Solar 303 505-8760 On 3/31/21 12:48 PM, William

Re: [RE-wrenches] Converting a old Troybuilt Roto tiller

2021-03-26 Thread Ray
ting surge. Or you could go 21st century, with 48v, Li+ PWM controller, etc  Another option to consider is using existing Li+ battery packs, like Ryobi's 40 v lawn mower packs. Ray Walters Remote Solar 303 505-8760 On 3/26/21 5:32 PM, Dana Orzel wrote: Hey All wise ones, I have an

Re: [RE-wrenches] Outback settings adjustment so batteries consume less of PV output

2021-03-19 Thread Ray
How big is the battery bank? How old is it?  It doesn't look that far off of what I've seen in GTB systems. Ray Walters Remote Solar 303 505-8760 On 3/19/21 12:21 PM, Christopher Warfel wrote: I have not been able to find a way to set my customers battery charging parameters so that the AGM