Re: [RE-wrenches] Suntech 175W 24V Module

2010-11-09 Thread Starlight Solar Power Systems
Davis, I have one in stock. Call me. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 - Original Message - From: Davis Terrell To: re-wrenches@lists.re-wrenches.org Sent: Friday, November 05, 2010 4:58 AM Subject: [RE-wrenches] Suntech 175W 24V Module

Re: [RE-wrenches] Off grid DC Loads: DC Converter

2018-01-16 Thread Starlight Solar Power Systems
I too would like to know the make and model of batteries that are loosing capacity. In the past 5 years we have experienced abnormally high failures from 2 brands. Larry On Jan 15, 2018, at 2:00 PM, Jay wrote: Can you tell us: Battery make,model and size? Jay Peltz power. On Jan 15, 2018

[RE-wrenches] Concorde Lifeline Battery failures

2018-01-19 Thread Starlight Solar Power Systems
issues. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Jan 18, 2018, at 9:18 AM, Drake wrote: A Concorde AGM PVX 3050T recently failed in a bank of 8. Larry mentioned a couple of brands experiencing problems. These batteries are 4 years old and have been kept

Re: [RE-wrenches] has anyone ever had this happen?

2018-01-23 Thread Starlight Solar Power Systems
done either as they were just fantasies to begin with. Larry Crutcher Starlight Solar Power Systems On Jan 23, 2018, at 11:48 AM, jay wrote: HI All, I’ve had a large company want to do a project and they want me to invoice it as follows. They said it had to do with knowing the cost of

Re: [RE-wrenches] Li+ Systems Puerto Rico

2018-02-19 Thread Starlight Solar Power Systems
be a catch. Do you have any information about testing or a copy of their warranty? Larry Crutcher Starlight Solar Power Systems On Feb 19, 2018, at 4:10 PM, Kirpal wrote: Blue Planet - Lithium Iron Phosphate batteries are a good option for off grid and work very well with the Outback

Re: [RE-wrenches] Li+ Systems Puerto Rico

2018-02-20 Thread Starlight Solar Power Systems
will use a battery like that on the other. Besides, in a decade or so, will Li-ion battery cost make lead batteries a relic? IMO, lead is dead…or at least dying…slowly. Larry Crutcher Starlight Solar Power Systems On Feb 20, 2018, at 9:02 AM, Kirpal wrote: Larryyes those are big

Re: [RE-wrenches] heating a lithium battery bank

2018-02-26 Thread Starlight Solar Power Systems
ith-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w <https://www.ebay.com/itm/Digital-STC-1000-All-Purpose-Temperature-Controller-Thermostat-With-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w> Larry Crutcher Starlight Solar Power Systems On Feb 26, 2018, at 9:56 AM, Daniel Youn

Re: [RE-wrenches] heating a lithium battery bank; Danger of charging frozen

2018-02-26 Thread Starlight Solar Power Systems
inhibit controls that prevent charge current when a cell is below freezing. Larry Crutcher Starlight Solar Power Systems On Feb 26, 2018, at 12:09 PM, Darryl Thayer wrote: Hi Daniel and Larry, I have a LI-FePO system, Simpliphy 10 kWh it is on its third winter, the batteries are

Re: [RE-wrenches] heating a lithium battery bank

2018-02-27 Thread Starlight Solar Power Systems
know our product and educate the customer. Too often, this does not happen. Larry Crutcher Starlight Solar Power Systems On Feb 27, 2018, at 7:11 AM, drake.chamber...@redwoodalliance.org wrote: Snow on the array could be a very big problem with the heater load, inverter idle current and

Re: [RE-wrenches] heating a lithium battery bank

2018-02-28 Thread Starlight Solar Power Systems
a bit too much,…” Quote “…best to just isolate the battery bank if below 32-35F..." As I mentioned, these features are already built into the Li EMS system of 2 brands that we sell and likely other brands. No need to reinvent it. Larry Crutcher Starlight Solar Power Systems On Feb

Re: [RE-wrenches] Pump LCBs

2018-02-28 Thread Starlight Solar Power Systems
Hey Chris, Might be a long-shot but check with Frank at BZ Products. Rings a bell but can’t think why. Larry Crutcher Starlight Solar Power Systems On Feb 28, 2018, at 1:22 PM, ch...@oasismontana.com wrote: Dear people: I have a fellow looking for a supplier of LCBs for their PV pumping

Re: [RE-wrenches] Stuck in a furl

2018-03-07 Thread Starlight Solar Power Systems
Crutcher Starlight Solar Power Systems On Mar 7, 2018, at 12:42 PM, Mac Lewis wrote: Hello wrenches, I have a client with an older Whisper 200, 1 kW wind turbine. We didn't install this but have taken over the site maintenance since the original installer left town. The site rec

Re: [RE-wrenches] Chevy Bolt

2018-04-23 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Apr 23, 2018, at 11:33 AM, RE Ellison wrote: I have a customer with a 20-year-old modified sine wave inverter that has been no issue at all until recently when he arrived from New York City with his Chevy bolt Obviously the Bolt will not tolerate the modified sine

Re: [RE-wrenches] Fire damage

2018-05-04 Thread Starlight Solar Power Systems
mmend cheap instead. Larry Crutcher Starlight Solar Power Systems On May 4, 2018, at 10:07 AM, Kristopher Schmid wrote: Greetings wrenches, I have a client that is looking to buy some salvaged modules off of a building that was near a fire. What kind of potential issues can you antic

[RE-wrenches] Fullriver Battery meltdown

2018-05-10 Thread Starlight Solar Power Systems
. Fullriver would not allow anything towards replacement do to the reporting date being grater than 24 months. I would like to know has anyone else had a similar failure with Rolls or Fullriver AGM batteries, specifically L16 size. Thank you, Larry Crutcher Starlight Solar Power Systems

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
used? Was it a bus system? Absorb with End Amps was turned on? Sent from my iPhone On May 10, 2018, at 4:41 PM, Michael Morningstar mailto:mjmornings...@gmail.com>> wrote: > > One year old. Well looked after system. > On May 10, 2018, at 1:42 PM, Starlight Solar Power Syste

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
I agree….that is something we have never done. These batteries are same date and both new when installed. Larry On May 10, 2018, at 3:49 PM, Rick Brown wrote: I’m inclined to agree with Maverick. Mixing old and new batteries is not recommended. Differing internal resistance coupled with po

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On May 10, 2018, at 1:59 PM, Steve Higgins wrote: Larry, Do you have any pic's of them installed? That would help a lot in getting an idea of how/why these failed. I do have two questions for you... Were there tie down straps over the tops of the batt

Re: [RE-wrenches] Disappearing Thread

2018-05-11 Thread Starlight Solar Power Systems
I have sent 4 replies and none are showing. Larry On May 11, 2018, at 10:32 AM, Mark Frye wrote: Could have sworn there was a thread here about melted batteries, but it not showing in my email client anymore. ___ List sponsored by Redwood Alliance

Re: [RE-wrenches] Disappearing Thread

2018-05-11 Thread Starlight Solar Power Systems
Sorry…to fast on reply…I have received the messages I sent. Larry Crutcher On May 11, 2018, at 10:35 AM, Starlight Solar Power Systems wrote: I have sent 4 replies and none are showing. Larry On May 11, 2018, at 10:32 AM, Mark Frye wrote: Could have sworn there was a thread here

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
Steve, Here is another similar installation. There is air space on top of and some between the battery. Many of our installations have the AGM batteries completely sealed in a box. 17 years of installing battery systems like this and not one single problem. Larry Crutcher Starlight Solar

Re: [RE-wrenches] Small system lithium or equivalent battery technology

2018-06-07 Thread Starlight Solar Power Systems
http://www.lifebluebattery.com/rv-boat-lithium-ion-batteries/index.html Bluetooth communications with the EMS built in. On Jun 7, 2018, at 11:56 AM, cwarfel wrote: I am trying to redesign a couple hundred watt load off-grid system by first focusing on the battery technology. The Li based

Re: [RE-wrenches] Lithionics Batteries

2018-08-16 Thread Starlight Solar Power Systems
are simple ways to continue using the battery until it is repaired. Much happier customer. You can contact me off the list or call if you would like further advise. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Aug 16, 2018, at 2:51 PM, Jason Szumlanski wrote

Re: [RE-wrenches] Lithionics Batteries

2018-08-16 Thread Starlight Solar Power Systems
ything is field serviceable and if the EMS does turn off, there are simple ways to continue using the battery until it is repaired. Much happier customer. You can contact me off the list or call if you would like further advise. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 34

Re: [RE-wrenches] SOC, FNDC, and LFP batteries

2018-08-18 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Aug 17, 2018, at 12:09 PM, Lou Russo wrote: Hello All, Does anybody have any insight in getting the SOC to report accurately on the Outback FNDC when using batteries that have a minimal voltage curve? I have several systems with LFP batteries that have both a

Re: [RE-wrenches] SOC and LFP batteries and TriMetric

2018-08-21 Thread Starlight Solar Power Systems
myths. Careful what you read. Larry Crutcher Starlight Solar Power Systems On Aug 21, 2018, at 12:26 PM, Sindelar Solar wrote: Yes, I just did. Ralph retired last year and I spoke with the new owner. In short, little change - use 2% of capacity for amp threshold and set CEF to 98% from

Re: [RE-wrenches] three-phase storage

2018-08-30 Thread Starlight Solar Power Systems
discounts to wrenches. Thank you, Larry Crutcher Starlight Solar Power Systems On Aug 30, 2018, at 10:37 AM, Marco Mangelsdorf wrote: Aloha all, I’m on the hunt for three-phase storage @ 277/480V. Yes, Tesla has its Powerpack. But availability is questionable. I’m open to suggestions

Re: [RE-wrenches] Batt Cap AGM...equalizing AGM

2018-11-23 Thread Starlight Solar Power Systems
been recombined, these areas are targeted for recombination. Slowing the growth of irreversible sulfation results in retaining higher capacity and thus longer cycle life. Just my opinion developed over the years it took me to acquire a gray beard. Larry Crutcher Starlight Solar Power Systems On N

Re: [RE-wrenches] Infinia Stirling linear alternators generators

2018-11-24 Thread Starlight Solar Power Systems
Thank you Hilton and Darryl. That explains what I’m seeing here in Yuma: A 90kW installation that went slowly, and is now entirely, off line. These are the linear alternator design. Any chance your friend will have technical documents? Larry On Nov 24, 2018, at 11:37 AM, Hilton Dier wrote:

Re: [RE-wrenches] FullRiver battery question

2018-11-29 Thread Starlight Solar Power Systems
Let me confirm what William has shared about Deka/MK 8D AGM batteries; they have a very high failure rate. We saw over 40% fail within 2-3 years of installation. Deka would not own up to the problem and offered no compensation. Fullriver has been the finest AGM we have ever sold. All DC models a

Re: [RE-wrenches] Lithium battery cost

2018-12-21 Thread Starlight Solar Power Systems
. Larry Crutcher Starlight Solar Power Systems On Dec 20, 2018, at 6:05 PM, Jay wrote: Hi all, I was doing some research on the Chevy bolt, and found that it’s battery cost about $145 per kWh in 2015. All the batteries I can find for sale for offgrid small systems ( 10-100 kWh) are in the

Re: [RE-wrenches] LiFePo4 vs BOS

2019-01-07 Thread Starlight Solar Power Systems
Howie, We have many hundreds of Li battery systems sold and installed. Never had any failure of PV controllers including Outback due to charging Li-ion. Larry Crutcher Starlight Solar Power Systems On Jan 7, 2019, at 11:23 AM, Howie Michaelson wrote: Hey Dan, Are you saying that OB is

Re: [RE-wrenches] LiFePo4 vs BOS

2019-01-08 Thread Starlight Solar Power Systems
protection opens. We mostly sell Midnite and Blue Sky Energy controllers with some Outback in the mix. No failures have been reported to us. Larry Crutcher Starlight Solar Power Systems On Jan 7, 2019, at 7:46 AM, d...@foxfire-energy.com wrote: I've been asked to trouble shoot a problem

Re: [RE-wrenches] Multiple inverters

2019-02-27 Thread Starlight Solar Power Systems
William, It seems this question needs to be addressed: What is the intended meaning of “installed in one system” in 2014? If you have separate “systems”, they should not be governed by 705.12. So, at what point does a “system” begin and end? PV modules to the disconnect? ...to the load panel? .

Re: [RE-wrenches] DKD Lithium Batteries

2019-03-04 Thread Starlight Solar Power Systems
e low and high voltage disconnect, it may be a dangerous battery without external control. Did you get that release form yet? Just FYI about us, since 2013 we have designed and sold Li battery power systems now numbering hundreds of customers. Larry Crutcher Starlight Solar Power Systems O

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Apr 19, 2019, at 10:27 AM, Mac Lewis wrote: Hello Wrenches, We recently inherited an Outback system that I've been keeping an eye on via Optics. Its a dual stack 3648 VFXR, with about 4kW of PV with a single string of EnergyCell 1100RE battery

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-22 Thread Starlight Solar Power Systems
higher loads or a greater percentage of capacity loss. I was just trying to give a more accurate consumption total to compare voltage. Larry Crutcher Starlight Solar Power Systems On Apr 19, 2019, at 4:14 PM, Glenn Burt wrote: Hi Larry, I am curious why you would use the 100Hr rate for this

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
Hi Drake,The way I wire them is to place them side by side and flip every other battery 180°. Then you can use a interconnect cable without tight bends. I attached a diagram as it is easier to see than to describe.Larry CrutcherStarlight Solar Power Systems untitled.pdf Description: Adobe PDF docu

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
Sorry Drake, I should read better…you said Concorde. Larry On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems wrote: Hi Drake, The way I wire them is to place them side by side and flip every other battery 180°. Then you can use a interconnect cable without tight bends. I attached

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Sorry Drake, I should read better…you said Concorde. Larry On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Hi Drake,The way I wire them is to place them side by side and flip

Re: [RE-wrenches] Lithium Batteries - Li-ion battery warning

2019-05-03 Thread Starlight Solar Power Systems
revent charge current when below freezing. Larry Crutcher Starlight Solar Power Systems On May 3, 2019, at 12:45 PM, Howie Michaelson wrote: Hi Folks, About to spec my first Lithium battery backup job. The client is not a heavy user, but wants things done right more than being totally cost ef

Re: [RE-wrenches] heating lithium in cold weather

2019-05-17 Thread Starlight Solar Power Systems
internal BMS. You can build a box and add a silicone type heater with a temp controller. I’ve bought items like that on eBay for about $25. See photo. Larry Crutcher Starlight Solar Power Systems On May 16, 2019, at 4:41 PM, jay wrote: HI All, I”m wondering if anyone has suggestions about how to

Re: [RE-wrenches] Large off-grid inverter/storage

2019-09-06 Thread Starlight Solar Power Systems
fully charge them, for offgrid use, the advantages are huge. For people making growing weeds, buy the best. Contact me off the list if you would like more understanding about Li battery storage. Larry Crutcher Starlight Solar Power Systems la...@starlightsolar.com On Sep 6, 2019, at 9:32

Re: [RE-wrenches] Honda EU2000i output V adjustment - Magnum Energy

2019-09-24 Thread Starlight Solar Power Systems
charge rate to about 50% or less, they work flawlessly. Larry Crutcher Starlight Solar Power Systems On Sep 24, 2019, at 8:30 AM, Dave Angelini Offgrid Solar wrote: We ended up usine a 50 foot #14 extension cord and the drop got the 2000i to play nice with the magnum. Outback and

Re: [RE-wrenches] Honda EU2000i output V adjustment - Magnum Energy

2019-09-24 Thread Starlight Solar Power Systems
above 125 Vac. Control boards are not to pricy and very easy to replace. Hope that helps. Larry Crutcher Starlight Solar Power Systems On Sep 24, 2019, at 9:39 AM, Starlight Solar Power Systems wrote: Hi Dave, I’m curious, can you describe the problem you had with a Magnum inverter and

Re: [RE-wrenches] 24 volt LiFePO4 Battery options

2019-09-27 Thread Starlight Solar Power Systems
to you Howie. Larry Crutcher Starlight Solar Power Systems On Sep 26, 2019, at 3:58 PM, Dave Angelini Offgrid Solar wrote: My 2 cents are each client is different and if they have been fine on that one set of batteries then do what is in their interest. An inverter is easily replaced. I

Re: [RE-wrenches] 600V DC contactor

2019-11-23 Thread Starlight Solar Power Systems
We have used Gigavac in some of our Li-ion EMS systems for many years with hundreds in the field and no failures. GX11 good to 800Vdc. https://www.gigavac.com/catalog/power-products/gx-series Larry Crutcher Starlight Solar Power Systems On Nov 22, 2019, at 8:47 PM, Chris Sparadeo wrote

Re: [RE-wrenches] Large Lithium 100 kWh-200kWh

2020-02-24 Thread Starlight Solar Power Systems
transfer to use in off grid power systems. Please reply off list if you need more info. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 sa...@starlightsolar.com On Feb 23, 2020, at 7:40 PM, Mac Lewis wrote: Hey wrenches, What are you using for Lithium in the 100 kWh-200 kWh range

Re: [RE-wrenches] 48 VDC Control fusing

2020-02-28 Thread Starlight Solar Power Systems
%7C2510416%2F2301910&a7=In%20Stock%20Only&n8744=1%20Pole&n11096=50%20VDC%2C48%20VDC 3A example: https://www.alliedelec.com/product/te-connectivity/w58-xb1a4a-3/70199433/ Larry Crutcher Starlight Solar Power Systems On Feb 28, 2020, at 12:35 PM, drake.chamber...@redwoodalliance.org w

Re: [RE-wrenches] Semi flexible modules

2020-03-09 Thread Starlight Solar Power Systems
long as you don’t expect the longevity of a framed, glass module. Customers using them occasionally as a portable module are experiencing long life. Larry Crutcher Starlight Solar Power Systems On Mar 8, 2020, at 4:02 PM, Jay wrote: Hi all, Especially those that do RV, Any recommendations

Re: [RE-wrenches] Semi flexible modules

2020-03-09 Thread Starlight Solar Power Systems
-PowerBond-112-Inch-15-5-Inch/dp/B002MWDI44 Larry Crutcher Starlight Solar Power Systems On Mar 9, 2020, at 11:07 AM, Ray wrote: I 2nd Larry's experience. I've never seen any flex modules that have held up for more than a few years. Complete degradation in our high a

Re: [RE-wrenches] Brown-Out Prone Opportunity Charging

2020-03-13 Thread Starlight Solar Power Systems
battery at 100%. Protect the PS with the appropriate AC surge or LV protection. With this setup your AC power is always on with no brownouts or loss of power. Larry Crutcher Starlight Solar Power Systems On Mar 13, 2020, at 12:02 PM, Jeff Clearwater wrote: Good Day Esteemed Wrenchers, So

Re: [RE-wrenches] Brown-Out Prone Opportunity Charging

2020-03-16 Thread Starlight Solar Power Systems
than you design for can be backed up with a generator. Larry Crutcher Starlight Solar Power Systems On Mar 13, 2020, at 6:09 PM, Jeff Clearwater wrote: Thanks All, Mick and Tump - I'll look into the Victron - good suggestion - Thanks! Chris - I'm not sure a transformer will buffer

Re: [RE-wrenches] Known residential/commercial fires from LI batteries

2020-04-13 Thread Starlight Solar Power Systems
sk me to name a brand, just study the product you use…for everyones good. Larry Crutcher Starlight Solar Power Systems On Apr 9, 2020, at 4:07 PM, Bruce Leininger wrote: Hi. I was wondering if there are any known instances of fires from residential or commercial storage systems. I'm spe

[RE-wrenches] MC4's in stock (missing MC4)

2010-03-25 Thread Starlight Solar Power Systems
I have 80 each MC4's available. PV-KST4/6II MALE6 - 9 mm gland range and 12 - 10 AWG conductor range PV-KST4/6II FEM6 - 9 mm gland range and 12 - 10 AWG conductor range Contact me off list. la...@starlightsolar.com Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Ma

Re: [RE-wrenches] PV excellent battery charger

2010-03-25 Thread Starlight Solar Power Systems
e has been recombined into lead, lead dioxide and sulphuric acid. There are pulsing circuits available but the PWM in a charge controller does not perform that function. So, why is PV power an excellent battery charger? Because it uses Starlight power! But you knew that. Larry Crutcher Starlight S

Re: [RE-wrenches] windenergy7

2010-04-01 Thread Starlight Solar Power Systems
eswiki.com/index.php/Directory:Home_Generation:Wind_Turbine Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing Address: 11881 S. Fortuna Road, #210 Yuma, AZ 85367 Retail Store & Shipping Address: 2998 Shari Ave. Yuma, Az 85365 - Original Message - From: Kirk Heran

Re: [RE-wrenches] KD135 source?

2010-04-20 Thread Starlight Solar Power Systems
Are you looking for grid tie or the J-box? I have some of the J-box 135's. Just FYI, the 135's are a larger module at 59.1 x 26.3. The discontinued 120's, 125's and 130's were all 56.1 x 25.7. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 Mailing Addre

Re: [RE-wrenches] Tiny load problem

2010-05-11 Thread Starlight Solar Power Systems
sine wave since many small load items like battery chargers, electric blanket control, electric toothbrush, etc., fail with MSW inverters. Contact me off list if you don't have a resource for small 12, 24 and 48 volt inverters. Larry Crutcher Starlight Solar Power Systems (928) 342-910

Re: [RE-wrenches] LiFePo4

2014-09-16 Thread Starlight Solar Power Systems
ERROR….I meant to say ….reach 3.55 volts per cell. On Sep 16, 2014, at 9:43 AM, Larry Crutcher, Starlight Solar Power Systems wrote: Mac, Li-ion batteries are connected the same as any other deep cycle, positive and negative terminals. The Battery management is done actively on each cell

Re: [RE-wrenches] LiFePo4

2014-09-16 Thread Starlight Solar Power Systems
Jarmo, I must say I disagree with most of what you have said. In the EV DIY industry, there are a growing number of conversions using LFP battery banks without any BMS or EMS at all. These pioneers are risking there multi-thousand banks because they have learned something about these cells. The

Re: [RE-wrenches] LiFePo4

2014-09-17 Thread Starlight Solar Power Systems
William, What did you find at the site? I did not see any attachment or link in your email so let me know what you are working on. Do you have any questions about the batteries/system? Larry On Sep 16, 2014, at 12:31 AM, William Miller wrote: Friends: Here are the specific batteries I

Re: [RE-wrenches] LiFePo4

2014-09-18 Thread Starlight Solar Power Systems
William, This is one reason I choose to avoid the "black box" approach to Li-ion batteries for our customers. There are several companies offering enclosed battery/controls like the OES. Their approach does not match well to the off-grid and mobile markets that I serve. Since most LFP batteri

Re: [RE-wrenches] LiFePo4

2014-09-18 Thread Starlight Solar Power Systems
smaller lead acid battery in parallel with the LiFePo bank so the LiFePo contains most of the "energy" storage, but the LA can supply the surges and low impedance source voltage. boB On 9/18/2014 8:53 AM, Starlight Solar Power Systems wrote: > William, > > This is one reaso

Re: [RE-wrenches] LiFePo4

2014-09-18 Thread Starlight Solar Power Systems
27;s all a compromise. boB On 9/18/2014 10:55 AM, Starlight Solar Power Systems wrote: > boB, > > When charging a LFP battery, the charge terminates when absorb voltage is > reached unless you have an enormous charger in which case you will need to > terminate based on AH returne

Re: [RE-wrenches] LiFePo4

2014-09-18 Thread Starlight Solar Power Systems
gh to be called "off". Couldn't be easier. Now we're just talking price compared to a tried and true LA battery ? Some may remember Boeing's little problem recently though and that may turn them off. boB On 9/18/2014 11:33 AM, Starlight Solar Power Systems wrote: >

Re: [RE-wrenches] SWRC for older Power Series inverter

2014-10-06 Thread Starlight Solar Power Systems
Hi Chris, We still have stock on the RC6, RC7 and RC7GS that came before the RC/GS. These all work with the old RV and Legend series inverters. I will be back in Az in about 1 week if you still need one. Larry On Oct 6, 2014, at 9:37 AM, Chris Daum wrote: Dear people: Does anyone have the

Re: [RE-wrenches] SWRC for older Power Series inverter

2014-10-06 Thread Starlight Solar Power Systems
After re-reading it looks like you’re not wanting the RC remotes but rather the remote option for the PS series. So, as Roseanne Roseannadanna would say…..never mind. On Oct 6, 2014, at 5:20 PM, Starlight Solar Power Systems wrote: Hi Chris, We still have stock on the RC6, RC7 and RC7GS

Re: [RE-wrenches] Quantifying power quality

2014-10-12 Thread Starlight Solar Power Systems
Hi William, If you recall a couple years ago we had some discussion here about a problem with a specific make appliance being powered by a Magnum inverter. The problem, it was discovered, was the appliance input PF was creating current demands that the transformer based inverter could not keep

Re: [RE-wrenches] SMA DC Disconnect Switch failure

2014-10-16 Thread Starlight Solar Power Systems
marco, SMA has agreed to replace it. Have you had any trouble with the replacement disco(s)? On Oct 16, 2014, at 2:24 PM, Marco Mangelsdorf wrote: Yes, I’ve had a number fail over the years, especially the no-longer-made DC/AC combo switches. I’d get a warranty replacement from SMA…if it’s

Re: [RE-wrenches] magnum question

2014-10-24 Thread Starlight Solar Power Systems,
Jay, Perhaps asking the question here. I have hundreds of Magnum inverter installations, perhaps I or others can help. Larry On Oct 23, 2014, at 5:44 PM, jay peltz wrote: HI All, Does anyone have a person at Magnum in engineering or higher up than tech support. I've got a problem with an i

Re: [RE-wrenches] warranty exclusions

2014-10-25 Thread Starlight Solar Power Systems,
Rebecca, This reminds me of a Sanyo grid tie system we quoted years ago to be installed in Yuma, AZ. After receiving the PV modules (11kW), I discovered that the warranty was void if the average temperature was above 104° F (40C). That means “no warranty” in Yuma and much of the desert SW. For

Re: [RE-wrenches] Passive Battery Venting

2014-10-29 Thread Starlight Solar Power Systems,
I too saw that these were AGMS. The only time excess H venting happens is with severe over voltage for a period of time. How often will this happen? Have any battery wrenches experienced high volume venting of AGM’s? Our experience: There is no NEC requirements for mobile installations. We have

Re: [RE-wrenches] Voltage Degradation with Uni-Solar laminate

2015-06-01 Thread Starlight Solar Power Systems
Luke, For reference, we sold/installed many hundreds of Uni-Solar products since 2002. I have never seen anywhere near that much Voc loss. Since the PVL-68 has an open circuit of 23.1V (92.4V) but you only see 14.2V (71V), a loss of 25%, I do not believe degradation is the culprit even at 15

Re: [RE-wrenches] Voltage Degradation with Uni-Solar laminate

2015-06-01 Thread Starlight Solar Power Systems
Sorry...I meant to type 17.75V (71V). On Jun 1, 2015, at 11:21 AM, Starlight Solar Power Systems wrote: Luke, For reference, we sold/installed many hundreds of Uni-Solar products since 2002. I have never seen anywhere near that much Voc loss. Since the PVL-68 has an open circuit of 23.1V

[RE-wrenches] Finally, a simple battery backup switch/controller

2015-06-01 Thread Starlight Solar Power Systems
Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive:

Re: [RE-wrenches] SnapNrack - Anti-seize

2015-06-29 Thread Starlight Solar Power Systems
You can use a thin sponge soaked anti-seize and just touch the threads to the sponge. Since it only takes a minute amount of lube to prevent galling, you can prep all your bolts in the shop and bag them. Zip lock the sponge for the next job. Larry Crutcher Starlight Solar Power Systems On

Re: [RE-wrenches] [SPAM] Re: Mate Drop and Charge Functions

2015-07-12 Thread Starlight Solar Power Systems
their new 100 amp charge controller, ME will have a complete solution through one remote. Larry Crutcher Starlight Solar Power Systems On Jul 12, 2015, at 4:37 PM, jay wrote: All the different remote controls have their pros/cons. However I find the web based videos from outback to be the most

Re: [RE-wrenches] Generac QT series

2015-07-14 Thread Starlight Solar Power Systems
photos so I believe your problem is not as simple as the sine waveform. From the cost standpoint, I’de guess you have to try a different brand inverter first. However, since the problem only occurs with that particular generator, I would not trust it. Larry Crutcher Starlight Solar Power Systems

Re: [RE-wrenches] Aquion Energy

2015-07-16 Thread Starlight Solar Power Systems
Hi Mark, There was some discussion back in November 2014 on this list. They claim 100% DoD but I can’t see how you can use the full capacity of the battery due to the broad operating voltage. Larry Crutcher Starlight Solar Power Systems On Jul 16, 2015, at 5:20 AM, Mark Frye wrote: Does

Re: [RE-wrenches] Trina Module Annual Degradation

2015-07-18 Thread Starlight Solar Power Systems
, Kyocera, 13 years after the 1 Year Limited Warranty expired, is STILL replacing the KC120 and 80 Watt modules with a rebuilt unit and they are STILL paying us labor to replace them. What a company! Larry Crutcher Starlight Solar Power Systems On Jul 18, 2015, at 11:09 AM, b...@midnitesolar.com

Re: [RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Starlight Solar Power Systems
e run. Larry Crutcher Starlight Solar Power Systems On Jul 22, 2015, at 10:37 AM, Jerry Shafer wrote: Wrenches Some time back there was discussion on the conductor size and efficiency rating requirement for long DC runs. What I am looking at is this, 400 feet of MCM 400 to keep the line loss

Re: [RE-wrenches] Using the North Facing Roof

2015-07-28 Thread Starlight Solar Power Systems
the north side. I can not see any benefit in AZ even at todays low prices. Now, if I were building in Quetzaltenango, Guatemala, that would be a different story. But then again, I would have to clean off the volcanic ash each morning. Larry Crutcher Starlight Solar Power Systems chart came from

Re: [RE-wrenches] Lithium Iron Phosphate

2015-08-18 Thread Starlight Solar Power Systems
ed to fully charge. Hopefully some RE equipment manufacturers will see this coming potential and design suitable chargers. Larry Crutcher Starlight Solar Power Systems On Aug 17, 2015, at 3:29 PM, Daniel Young wrote: Hello Wrenches, I’ve been trying to think through how I can mate some

Re: [RE-wrenches] Lithium Iron Phosphate

2015-08-18 Thread Starlight Solar Power Systems
challenge for equipment makers but can be resolved by designing CAN interface and software that communicates with chargers and control CPU’s to make the adjustments on the fly. Larry Crutcher Starlight Solar Power Systems On Aug 18, 2015, at 8:31 AM, Peter Parrish wrote: I too am interested in

Re: [RE-wrenches] Lithium Iron Phosphate

2015-08-18 Thread Starlight Solar Power Systems
software that communicates with chargers and control CPU’s to make the adjustments on the fly. Larry Crutcher Starlight Solar Power Systems On Aug 18, 2015, at 8:31 AM, Peter Parrish wrote: I too am interested in LiFeP batteries. I think we need some more information on charge/discharge cycles

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread Starlight Solar Power Systems
Ray, I’m curious about what you mean by not doing a 3 stage charge. While PV charging in coupled mode (off grid), the battery will reach your absorption set point. Is this triggering the GT inverters to shut off or does the battery inverter absorb timer run at all? I would think the absorb time

Re: [RE-wrenches] Control board Kohler 14 RES

2015-08-25 Thread Starlight Solar Power Systems
Magnum Energy inverters have no capability to send current to the grid (generator) through their inputs. Sounds like BS to me. What is this mystery board that blocks AC current one way? Larry On Aug 25, 2015, at 11:18 PM, Mac Lewis wrote: Hello wrenches, I've got an issue I'd like to put ou

Re: [RE-wrenches] Fronius Warranty Problems

2015-09-03 Thread Starlight Solar Power Systems
Peter, Fronius has some of the most ignorant people working for them. It took me over a year to receive payment for an inverter swap that they diagnosed as having failed. After I returned the old inverter they claimed nothing was wrong. Run from Fronius! Thank you, Larry On Sep 3, 2015, a

Re: [RE-wrenches] Morningstar PWM

2015-09-10 Thread Starlight Solar Power Systems
the battery not getting charged. Larry Crutcher Starlight Solar Power Systems On Sep 9, 2015, at 5:06 PM, Drake wrote: Hello Wrenches, I have a Morningstar PWM 45 that doesn't drop out of absorb. It is set with dip switches to absorb at 29.2 V and stays constant around 29.1. It has stay

Re: [RE-wrenches] Rooftop DC disconnects

2015-09-24 Thread Starlight Solar Power Systems
William and Wrenches, I have pondered situations like this one and wonder the following: If a high voltage DC solenoid were placed at the PV array and the coil was controlled by an arc fault detector along with a means of manually disconnecting, would that not work to satisfy shut down require

Re: [RE-wrenches] Rooftop DC disconnects

2015-09-24 Thread Starlight Solar Power Systems
Ray, UL508 for sure but look here: http://gigavac.com/catalog/pp/hx.html Larry On Sep 24, 2015, at 11:03 AM, Ray Walters wrote: …. Is the Gigavac UL listed? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 __

Re: [RE-wrenches] Rooftop DC disconnects

2015-09-24 Thread Starlight Solar Power Systems
the Gigavac UL listed? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 9/24/2015 10:45 AM, Starlight Solar Power Systems wrote: > William and Wrenches, > > I have pondered situations like this one and w

Re: [RE-wrenches] Rooftop DC disconnects

2015-09-25 Thread Starlight Solar Power Systems
on a two story house with a 6:12 roof pitch. Something to consider. Regards, Gary Willett PE Icarus Engineering On 9/24/15 7:26 PM, Starlight Solar Power Systems wrote: > William, Ray, > > I asked Midnite about using the Aux circuit for control for ground or arc > faults. They

Re: [RE-wrenches] Rooftop DC disconnects

2015-09-26 Thread Starlight Solar Power Systems
Hello Howie, I attached it to my email on 9-24-2015. In brief, a HV relay disconnects the PV array and optional relay disconnects the battery. Midnite plans to add the arc fault Aux feature. Here it is again: I asked Midnite about using the Aux circuit for control for ground or arc faults. Th

[RE-wrenches] Grid tie in Nicaragua

2015-09-29 Thread Starlight Solar Power Systems
Has anyone done a grid tie system in Nicaragua? I would appreciate talking about equipment reliability and other difficulity due to utility power instability. Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood

Re: [RE-wrenches] Five L16s in a 24V string?

2015-10-01 Thread Starlight Solar Power Systems
be lasting longer since they have half the DoD each day. A very strange setup, I’ve never seen this. Since I rarely see a true battery failure (most are damaged by the owner) I can’t say that I’ve noticed any pattern. Larry Crutcher Starlight Solar Power Systems On Sep 30, 2015, at 8:43 PM, Alla

Re: [RE-wrenches] Five L16s in a 24V string?

2015-10-01 Thread Starlight Solar Power Systems
Since multiple batteries failed ("the one that always fails"), did he buy one new battery each time and tie it to the old failing one? Or, did he start with a new bank and create the parallel at that time? Since he’s an “old timer” he may be mixing different age batteries in the bank. I see this

Re: [RE-wrenches] Five L16s in a 24V string?

2015-10-01 Thread Starlight Solar Power Systems
Took about a minute to draw with Pages on a Mac. On Oct 1, 2015, at 1:22 PM, Allan Sindelar wrote: ….Larry, nice drawing below. What did you use, as I need to learn it too? Allan Allan Sindelar al...@sindelarsolar.com NABCEP Ce

Re: [RE-wrenches] PV Tracker - Best available?

2015-10-03 Thread Starlight Solar Power Systems
is no space available for more PV it makes sense if you must have more production. Larry Crutcher Starlight Solar Power Systems On Oct 3, 2015, at 9:49 AM, SunHarvest wrote: Given 310# snow load in the Sierras, what are some suggestions for a superior pole-mounted tracking system? Right no