RE: dry grid prohibition

2012-06-11 Thread Reed Roisum
I am looking at the 1989 Handbook and it does state in 5-2.3.1 Volume Limitations. ...Gridded dry-pipe systems shall not be installed. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct www.ulteig.com -Original Message- From:

RE: solid unit load?

2012-05-22 Thread Reed Roisum
Todd, NFPA 13, 2010 ed. 3.9.2.8, Solid Unit Load of a Nonexpanded Plastic (Either Cartoned or Exposed). A load that does not have voids (air) within the load and that burns only on the exterior of the load; water from sprinkler might reach most surfaces available to burn. My guess is that an

RE: Indiana Codes

2012-05-15 Thread Reed Roisum
Here are the International Code adoptions by State... http://www.iccsafe.org/gr/pages/adoptions.aspx http://www.iccsafe.org/gr/documents/stateadoptions.pdf Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct www.ulteig.com -Original

RE: NICET Calculator for Advanced Hydraulics

2011-06-10 Thread Reed Roisum
Brian, I use the hp33s and I have all of the needed formulas on it and just have to punch in the missing variables. Maybe has more function than needed, but I like it. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct www.ulteig.com

RE: NICET Calculator for Advanced Hydraulics

2011-06-10 Thread Reed Roisum
Of Reed Roisum Sent: Friday, June 10, 2011 7:49 AM To: sprinklerforum@firesprinkler.org Subject: RE: NICET Calculator for Advanced Hydraulics Brian, I use the hp33s and I have all of the needed formulas on it and just have to punch in the missing variables. Maybe has more function than needed

RE: Why we have fire safety codes- MGM Grand - Nov 21 1980

2010-11-22 Thread Reed Roisum
You are right Ken. 119 souls. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 www.ulteig.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Parsley Consulting Sent:

RE: Re-Using Sprinklers

2010-10-25 Thread Reed Roisum
All I could find was 6.1.2.2 and 6.2.1 in 07 ed. Nothing about what you are referring to. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 www.ulteig.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Backflow Forward Flow Test

2010-10-04 Thread Reed Roisum
Check out NFPA 13, 2007 ed. A.8.17.4.6.1 also. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct 701.212.8810 cell www.ulteig.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Backflow Forward Flow Test

2010-10-04 Thread Reed Roisum
Jay, Check the archives as this topic has been talked about fairly often and recently. NFPA 13, 2007 ed. 10.10.2.5. We always spec a backflow test outlet (male threads) sized to be able to flow system demand. Contact me if you want more detail. Reed A. Roisum, CET Ulteig Engineers, Inc.

RE: Control Mode vs. ESFR

2010-09-23 Thread Reed Roisum
Even I know that IRAS are Individual Retirement Accounts. Didn't know you were required to have them though. And the way mine has been tanking lately maybe I'll try that ESFR thing. Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct

RE: Monitor nozzle

2010-09-20 Thread Reed Roisum
WOW! That's amazing Brad! Reed A. Roisum, CET Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct 701.212.8810 cell www.ulteig.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf

RE: Antifreeze

2010-09-13 Thread Reed Roisum
Brian, According to the International Plumbing Code the RPZ is required but can just isolate the portion of the system that has anti-freeze...i.e. doesn't need to be at the supply. 2006 IPC 608.16.4.1 Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: Wireless Tamper Switches?

2010-08-12 Thread Reed Roisum
http://www.worldelectronics.com/ This company claims to be the only one out there that has wireless systems for device monitoring?? I am sending for more information but prolly worth checking out. Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: heads in plastic bags

2010-08-12 Thread Reed Roisum
I bet Cahill has already begun his experiment...although I'm sure he is disappointed that he doesn't get to set fire to anything on this one. Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: membership segue that should be on Chat

2010-08-11 Thread Reed Roisum
Maybe AFSA should adopt the policy of AFAA (Automatic Fire Alarm Association) and require that you sign each post with whether or not you are a member or a guest. That way we could mark those that aren't members and send them nasty-grams a couple of times a year letting them know how dumb they

RE: 4-WAY BRACES

2010-08-10 Thread Reed Roisum
4-way bracing is required on all risers over 3 ft in length. A riser is defined as a vertical supply pipe. I assume you are wondering if a sprig needs to be 4-way braced if it is over 3 ft. in length? A sprig is a vertical supply pipes but it is also defined separately so I would say no you

RE: Test connection for forward flow testing of backflow

2010-07-26 Thread Reed Roisum
What if you don't have a fire pump and the system demand is more than what can be flowed out of the main drain (BTW, how do you measure the flow out of the main drain?) We typically spec a 2 1/2 single outlet (size and # of outlets dependent on the system demand), flush-type test connection

RE: Commentary/annex material

2010-07-19 Thread Reed Roisum
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Friday, July 16, 2010 9:03 AM To: sprinklerforum@firesprinkler.org Subject: RE: fire pump room - external door? Sorry I am so late to post. Note that the following is a should not a shall

RE: fire pump room - external door?

2010-07-16 Thread Reed Roisum
Sorry I am so late to post. Note that the following is a should not a shall... NFPA 20, 07 ed. A.5.12 ...Access to the pump room should be provided from outside the building... Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: 2009 IBC - Group R-4

2010-07-09 Thread Reed Roisum
Ken, Looks like a typo to me. I would guess the reference 903.2.7 was left over from IBC 2006 where it was Group R. Group R is now 903.2.8 and I'm guessing that is what 310.1 should be referencing. Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: short period spectral response

2010-07-09 Thread Reed Roisum
http://earthquake.usgs.gov Check out Ken Wagoner's AFSA webinar presentation from 10-30-08 (if it is available somewhere??). He walks through how to determine these numbers. Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: small room/closet

2010-07-08 Thread Reed Roisum
Todd, Not sure what you mean when you say 'when you use the small room rule', but any unprotected opening in a room produces a communicating space. I assume you are trying to determine whether to calculate the head in the closet when using the room design method?? Reed A. Roisum, CET Ulteig

RE: small room/closet

2010-07-08 Thread Reed Roisum
I believe you would include the sprinkler in the closet based on 11.2.3.3 (07 ed.)... ...calculations shall include the sprinklers in the room plus two sprinklers in the communicating space nearest each such unprotected opening unless the communicating space has ONLY ONE sprinkler, in which

RE: Question regarding NFPA 13 vs. NFPA 13R

2010-07-06 Thread Reed Roisum
IBC (ref. below 2006 ed.) allows 13R in Group I-1 if 4 stories or less. Note exception... [F] 903.2.5 Group I. An automatic sprinkler system shall be provided throughout buildings with a Group I fire area. Exception: An automatic sprinkler system installed in accordance with Section

RE: Hay Bale Storage

2010-07-01 Thread Reed Roisum
I think the purpose of the wrap is so the bales can be stored in the field but I'm sure some could wrap and store in a shelter too. Typically the wraps are plastic including a plastic net type wrap (mesh). Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From:

RE: Hay Bale Storage

2010-06-30 Thread Reed Roisum
And if baled too wet that mold can produce heat and eventually combustion. I don't know if this influences the protection scheme or not, but you could theoretically have a fire begin at the bottom of the stack (if it can get enough oxygen) and be quite large before producing enough heat to

RE: CPVC

2010-06-29 Thread Reed Roisum
I think he was making a funny. :) Reed A. Roisum, CET Ulteig Engineers, Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Tuesday, June 29, 2010 2:26 PM To:

RE: Gravity Tanks

2010-06-17 Thread Reed Roisum
So there is a use for differential equations. WOW. Guess I need to pay up. Reed A. Roisum, CET Ulteig Engineer, Inc. Engineering Technician Direct: (701)280-8580 Cell: (701)212-8810 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Stairways

2010-05-18 Thread Reed Roisum
straight through, awesome. I've always routed the pipe out and around a stairway. Thanks for the info. Brian Harris FDFP INC. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Tuesday, May 18

RE: Sprinkler temp

2010-05-06 Thread Reed Roisum
Chris, The commentary in A.6.2.5 ('07 ed.) says that sprinklers with the same temp. rating SHOULD be used in a given AREA, unless otherwise specified by 8.3.2. The word 'compartment' is used earlier in this 'blue' print but I would venture to say that the 18 beam does not separate this space

RE: Seismic Question

2010-05-05 Thread Reed Roisum
I'm sure someone that is from an area where the ground actually shakes every once in awhile can correct me on this, but I believe the site class is a designation given to an area based on the soil (e.g. hard rock, dense soil etc.). This factor along with others is used to determine the Seismic

RE: C-Factor

2010-04-20 Thread Reed Roisum
Table 9 in my FM Global Hydraulics Tables has Age Factors for public and fire pro mains and Table 6 has coefficients for underground piping based on age of pipe and water corrosiveness. Probably not what you are looking for though?? Reed A. Roisum, CET Engineering Technician Direct:

RE: Water stats

2010-04-15 Thread Reed Roisum
HFSC has usually got good stuff like that for residential...found one quick blurb... http://www.homefiresprinkler.org/newsletter/summer03/art10p2.html http://www.homefiresprinkler.org/FS/FSWaterUsage.html + Sprinkler systems discharged an average of 341 gallons of water per fire. +2,935 gallons

RE: Foam system piping

2010-04-14 Thread Reed Roisum
If it is military the concentrate lines are often (maybe always) required to be stainless steel. At least ETL 02-15 and 01-1-1 have that requirement. Reed A. Roisum, CET Engineering Technician Direct: (701)280-8580 Cell: (701)212-8810 -Original Message- From:

Steam for Fire Suppression

2010-04-12 Thread Reed Roisum
I don't have much information on this yet but here goes anyway... An owner of a manufacturing facility (I don't know what type of manufacturing) has in his head that he wants to use steam from his boiler for fire suppression (also don't know what he wants to protect). I am basically looking

RE: Steam for Fire Suppression

2010-04-12 Thread Reed Roisum
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Monday, April 12, 2010 10:19 AM To: sprinklerforum@firesprinkler.org Subject: Steam for Fire Suppression I don't have much information on this yet but here goes anyway... An owner

RE: Hard wired air compressors

2010-03-18 Thread Reed Roisum
The source is to be available at all times. This isn't necessarily talking about being movable or not. If it is able to be unplugged then it would not be available at that time that someone unplugs it. It wouldn't hurt to have some additional verbiage to clarify the intent here. I actually

RE: Backflow protection on antifreeze system

2010-03-11 Thread Reed Roisum
Ed, 2006 IPC 608.16.4.1 Additives or nonpotable source. Where systems under continuous pressure contain chemical additives or antifreeze, or where systems are connected to a nonpotable secondary water supply, the potable water supply shall be protected against backflow by a reduced pressure

RE: FDC LOCATION

2010-03-08 Thread Reed Roisum
If you are looking in NFPA 13 I don't think you will find it. Here is the reference in NFPA 14, 2007 edition: 6.4.5.4*Fire department connections shall be located not more than 100 ft (30.5 m) from the nearest fire hydrant connected to an approved water supply. Reed A. Roisum, CET Fire

RE: Cloud Protection

2010-03-05 Thread Reed Roisum
Jimmy, You said code reference and I'm not sure about that, but 8.15.1.2 '07 ed. has concealed spaces that do not require sprinkler protection. Spaces shall be considered concealed even with small openings such as those used for as return air for a plenum. Not sure if this is what you were

RE: Mansions in the Sky (No Place for NFPA Standards)

2010-02-02 Thread Reed Roisum
Are you going to sprinkler this new library? We wouldn't all of these priceless treasures getting wet!! Reed A. Roisum, CET Fire Protection Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct 701.212.8810 cell www.ulteig.com Energy | Water | Built-Environment

RE: dry system drains

2010-01-26 Thread Reed Roisum
8.16.2.5.3.1, 2007 ed. says that Aux. drains located in areas subject to freezing shall be readily accessible. I would take that to say no. Reed A. Roisum, CET Fire Protection Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct 701.212.8810 cell www.ulteig.com

RE: fire pump - 10 diameters

2009-12-09 Thread Reed Roisum
A.5.14.5 of NFPA 20 2007 ed. says that if the supply is from public water mains then the gate valve SHOULD be located as far as is practical from the suction flange. I'm not sure why because the commentary goes on to say that the gate valve does not interfere with the flow when it is fully

RE: RESIDENTIAL SPRINKLERS IN NFPA #13

2009-10-26 Thread Reed Roisum
You are allowed to go to NFPA 13R for I-1 occupancies. IBC 2006 903.2.5 Group I. An automatic sprinkler system shall be provided throughout buildings with a Group I fire area. Exception: An automatic sprinkler system installed in accordance with Section 903.3.1.2 or 903.3.1.3 shall be allowed

RE: Storage rooms in a office building

2009-09-21 Thread Reed Roisum
Sounds to me like OH2. I don't think the square footage of the room drives the classification?? Reed A. Roisum, CET Fire Protection Ulteig Engineers, Inc. 3350 38th Avenue S. Fargo, ND 58104 701.280.8580 direct 701.212.8810 cell www.ulteig.com Energy | Water | Built-Environment CONFIDENTIAL

RE: Fire Sprinker System Changes in Vis Lab

2009-09-04 Thread Reed Roisum
Jaber, What kind of advisement are you looking for? The plan for protecting this space with NOVEC 1230 and using VESDA early warning detection sounds like the way to go. Are you questioning removing the sprinkler system? You will most likely need AHJ approval to install only the clean agent

RE: Pockets

2009-08-20 Thread Reed Roisum
Geoff, A ceiling pocket could probably be defined as any elevation increase from the rest of the ceiling, but whether it needs to be sprinklered is probably what you are wondering?? I'm sure you have looked at 8.6.7.2 which has a long list of requirements that all have to be met in order to

RE: Pockets

2009-08-20 Thread Reed Roisum
deflectors are below the beams. Whew -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Thursday, August 20, 2009 6:28 PM To: 'sprinklerforum@firesprinkler.org' Subject: RE: Pockets Geoff

Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not required where a back-up engine driven or back-up steam turbine driven fire pump is installed in accordance with this standard. Does the use of an emergency generator serving only the fire pump (no other power) qualify as

RE: Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Thursday, August 20, 2009 4:18 PM To: 'sprinklerforum@firesprinkler.org' Subject: Fire Pump Alternate Power NFPA 20 (2007) Article 9.3.3 states An alternate source of power is not required where a back-up engine driven or back-up steam turbine driven fire pump

RE: Fire Pump Alternate Power

2009-08-20 Thread Reed Roisum
/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum Sent: Thursday, August 20, 2009 8:02 PM To: 'sprinklerforum@firesprinkler.org' Subject

RE: Gymnasium

2009-06-17 Thread Reed Roisum
Need more info... What code applies? What is the occupancy classification? Is there spectator seating? What is the square footage? Occupant load? Is it on a the floor level of exit discharge? Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South

RE: Gymnasium

2009-06-17 Thread Reed Roisum
? Probably about 150 people. On Wed, Jun 17, 2009 at 12:17 PM, Reed Roisum reed.roi...@ulteig.comwrote: Need more info... What code applies? What is the occupancy classification? Is there spectator seating? What is the square footage? Occupant load? Is it on a the floor level of exit discharge

RE: 100ft from FDC to hydrant?

2009-04-09 Thread Reed Roisum
NFPA 13, 2007 ed. Handbook 6.8 Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Factory Mutual: Remote Inspectors Test on wet system

2009-04-06 Thread Reed Roisum
FM seems to prefer the test connection to be at the remote branch line, but it is a should not shall. Check out Data Sheet 2-8n A-4-15.4.2. Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile:

RE: side by side standpipes

2009-03-25 Thread Reed Roisum
What Tom, Cliff, and Steve said. Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -Original Message- From:

RE: Another save, in Oregon

2009-03-06 Thread Reed Roisum
That was refreshing to read. I sent KTVZ a note telling them so. I especially like this line, The sprinkler system was shut down by the firefighters, who found no water damage. Since the economy is so bad, maybe Leyton is moonlighting as a reporter. Reed A. Roisum, CET Fire Protection

RE: system review

2009-02-27 Thread Reed Roisum
Can I suggest we use another career politician's name as a substitute for numnut? You know, someone that the only thing they are good at and understand is politics. I've got a few in mind. I am enjoying the Pelosi term...hoping it'll catch on outside the forum. :) Reed A. Roisum, CET Fire

RE: quote of the day

2009-02-04 Thread Reed Roisum
A pulse. Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Electrical Rooms

2008-12-16 Thread Reed Roisum
Brian, 8.15.10.3 2007 ed. Talks about the criteria you must have to eliminate sprinklers from an electrical room. The NEC prohibits running piping in the dedicated electrical space 110.26 2008 ed. 8.15.3 2007 ed. Discusses stairways. Not sure what you are looking for. IBC 1020.1.2 2006

RE: Collapsing File Storage System

2008-11-21 Thread Reed Roisum
Russell, Check out the commentary on 8.15.9 (2007 ed.). You can determine whether you are dealing with high-density mobile shelving. But that is kind of what it sounds like. Note what you need to do if you don't have 18 clear. Reed A. Roisum, CET Fire Protection Technician Ulteig

RE: Sprinkler Main Protection

2008-11-17 Thread Reed Roisum
PROTECTED] http://www.ch2m.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum Sent: Friday, November 14, 2008 6:08 PM To: 'sprinklerforum@firesprinkler.org' Subject: RE: Sprinkler Main Protection No, the area the main passes through

RE: overhang concealed space

2008-10-01 Thread Reed Roisum
Todd, I had the same argument with an architect a few weeks ago and I posted the question to the forum (Subject: combustible overhang 8-18-08) to see how this is typically handled. I didn't get any responses. Typically, the space can't be filled with insulation because it needs to remain

RE: FM-200 enclosure volume (Exclude Cabinets volume?) MY CONCLUSION!

2008-09-04 Thread Reed Roisum
Reza, I wouldn't necessarily say the 'right' choice, but certainly it is one of many good choices depending on the specific application and a number of factors. It seems as though many use 'FM-200' in lieu of 'Clean Agent' like we use 'Kleenex' for 'tissue'. There are many options when

RE: Small tanks

2008-09-03 Thread Reed Roisum
Chris, I came across this site when looking for tank manufacturers awhile ago. http://www.firewatersystemsinc.com/ Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office:

RE: FM-200 enclosure volume (Exclude Cabinets volume?)

2008-09-03 Thread Reed Roisum
Each of the clean agent gases have a NOAEL (No Observable Adverse Effect Level) number that they have been tested to. For example, the NOAEL % for Novec 1230 is 10%, (this means that they have exposed an animal to that concentration with no observable adverse effects) and the design

RE: Sprinklerforum Digest, Vol 34, Issue 25 ITEM #1

2008-08-28 Thread Reed Roisum
The strainer is only required on k factors smaller than 2.8k. [8.3.4.1] Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -Original Message- From:

Combustible Overhang

2008-08-18 Thread Reed Roisum
I checked the archives and couldn't find anything regarding this specific issue. I've got a 3'-0 overhang with combustible construction. The attic space has 18 of insulation with insulation stops at the edge of the building so the soffit (overhang) space is open for venting. The attic space

Air Compressor Power Supply

2008-07-24 Thread Reed Roisum
A building (nursing home) with an emergency generator has a dry system. Is the air compressor required to be connected to the emergency generator? NFPA-13 (2007) 7.2.6.2.1,2 says that the air supply shall be from a source available at all times and shall be capable of restoring normal air

RE: Stage's

2008-04-23 Thread Reed Roisum
If a water curtain is required for the proscenium opneing the design criteria is in 11.3.3. Reed A. Roisum Fire Protection Technician NICET Level III   Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079   Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500

RE: fitting rating

2008-04-17 Thread Reed Roisum
I believe the DN is Diameter Nominal. 300 DN (metric) is 300 MM which is a 12 NPS (Nominal Pipe Size - inches) Reed A. Roisum Fire Protection Technician NICET Level III Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main

RE: fm200 vs sprinkerls

2008-04-08 Thread Reed Roisum
The IBC reads that it is up to the fire code official if alternative fire extinguishing systems are allowed in lieu of the required automatic sprinklers. Reed A. Roisum Fire Protection Technician NICET Level III Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number:

Diesel Fire Pump Fuel Tank

2007-12-28 Thread Reed Roisum
I am designing a fire pump room that has (2) diesel fire pumps that each have a 187 gallon fuel tank. My question is about containment. I was told by a fire pump supplier to use a double wall tank because it might eliminate the need for containment walls. Based on NFPA-37 6.3.2.4 it appears

RE: Seismic Bracing/Drops

2007-11-01 Thread Reed Roisum
If you have a handbook, look at the commentary text on 9.3.6.6. It says that the restraint talked about in 9.3.6.6 does not apply to drops to individual sprinklers. I don't think you are overlooking anything, but you should take into consideration that I come from probably the least active

RE: 10' Separation for Ceiling Pockets

2007-10-17 Thread Reed Roisum
Since no one else wants to 'tackle' this question... No, when determining whether you can omit sprinklers in the ceiling pockets the requirements would just apply to ceiling pockets within the same room. Reed A. Roisum Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South

RE: Proposal Form

2007-10-03 Thread Reed Roisum
http://www.nfpa.org/assets/files/PDF/CodesStandards/NFPAProposalForm.doc You might have to be a NFPA member to get to this document?? Reed A. Roisum Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810

RE: CAD/PDF

2007-05-01 Thread Reed Roisum
Bluebeam works well. Not sure on cost. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: Tuesday, May 01, 2007 8:42 AM To: sprinklerforum@firesprinkler.org Subject: CAD/PDF Any good recommendations for a CAD to PDF converter?

Underground Dry Pipe

2007-04-17 Thread Reed Roisum
should I spec for the dry underground? Can (should) I use galvanized? Do you sleeve it? Any other suggestions? Thanks, Reed Roisum Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 ___ Sprinklerforum

RE: Underground Dry Pipe

2007-04-17 Thread Reed Roisum
system for the amphitheatre. The question is what pipe should I spec for the dry underground? Can (should) I use galvanized? Do you sleeve it? Any other suggestions? Thanks, Reed Roisum Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079

Calculating Attic Heads

2007-03-08 Thread Reed Roisum
I am reviewing a dry system attic layout using Tyco's Single Directional (SD) and Back to Back (BB) attic heads. The attic narrows at the remote area so that the peak goes from an attic peak (12/4 slope)with roof on each side, to a roof only on one side of the peak. (sorry for the poor

RE: Sprinkler Piping in Unsprinklered Areas

2007-01-18 Thread Reed Roisum
John, 8.15.3.3 (2002 ed.) may be what you are looking for. Reed Roisum -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, January 18, 2007 7:52 AM To: sprinklerforum@firesprinkler.org Subject: Sprinkler Piping

RE: M.I.C

2007-01-17 Thread Reed Roisum
Sorry Paul. Your answer is incorrect. You didn't phrase it in the form of a question. The correct answer is, What is Microbiologically Influenced Corrosion. We also would have accepted, What is Malaysian Indian Congress. Reed Roisum Fire Protection Department Ulteig Engineers, Inc. 3350