[Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

2022-03-21 Thread bill . brooks brooksfpe . com
Referring to the 2013 edition, wouldn’t an Annex note to 23.4.2.1.1 be exactly 
the thing that’s needed?  Still time to propose for next edition I think.  Get 
all this out into the open where the PhD wordsmiths can wrestle it to the 
ground.

Bill Brooks (memberr)

William N. Brooks P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410 544 3620 o
412-400-6528 c

From: Steve Leyton 
Sent: Monday, March 21, 2022 2:40 PM
To: Brad Casterline ; BRUCE VERHEI 
; Byron Weisz ; Michael de Gabriele 
; Sprinkler Academy - C Bilbo 
Cc: travis.m...@mfpdesign.com; sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

While I appreciate your insatiable curiosity and enthusiasm for what most 
consider the minutia of hydraulics, I caution that references to 
unsubstantiated preferences isn’t a particularly precise way of presenting 
technical content, especially when it’s this nuanced.

When I’m modeling a sprinkler system or private fire main system (two things 
I’ve very experienced with and that my firm does on a multiple-times-per-day 
basis), the only things I need to feel good about are:  conformance with basis 
of design criteria and applicable standards for the work in question; safety 
factor; cost-impact analysis of our proposed design.   Suggesting that 12 FPS 
is a feel-good criterion isn’t based on any particular scientific method that I 
can tell, so let’s leave that out of it.

As Byron astutely noted last week, fire protection demands are not continuous 
flows.   In fact, “Continuous Flow” is a defined term in AWWA standards, as is 
“Intermittent Flow”.   Since continuous flow is 24/7/365, we are an 
intermittent flow, as are fire hydrant flows, tank fills, pump tests and every 
other aspect of below-ground and overhead water-based systems.   The only 
reason that water districts care about velocity is that public main systems are 
more likely to experience surges and hammer phenomena at higher flow speeds.   
But we’re not a continuously flowing demand, we’re a closed system that sits 
static for 99.6735% of its lifetime and when called upon to activate (and with 
open nozzles, sprinklers, hydrant ports) we are highly unlikely to experience 
the rebounding pressure spikes of a hammer except potentially when that demand 
is shut off.Hammer in sprinkler systems has historically been caused by 
surges imposed on systems from outside sources.  (Also and by the way, 
regarding the continuous/intermittent thing, the fact that residential systems 
are a 7-10 minute event by rule, the restricting of meters to the limits of 
their continuous flow rating is BS.)

If the water gets to the emitter and the hydraulics of the design work within 
the parameters of the basis of design and good/best practices, then as Bruce 
might say, I don’t give a ___ about velocity because its NOT a codified 
metric and allowing any measure of subjectivity into the exercises – ESPECIALLY 
when it leaks into the enforcement side of the exercise – is not a good 
practice and should be disregarded.


Steve Leyton, President
Protection Design and Consulting
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.protectiondesign.com_=DwMGaQ=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM=iih4NVEkD89x14qk7m6LbFsl49j-eQ0kuCE55fl2VOI=axXgb8Run8Bdi8a6Oo1kuX0MIWmMUJg2kXBS8i3EFq8=EMYV-FWb9iPpplNapuyc_mqMAPGkWod0SXQ0DBzeuyI=>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training




From: Brad Casterline mailto:bcasterl...@fsc-inc.com>>
Sent: Monday, March 21, 2022 7:11 AM
To: BRUCE VERHEI mailto:bver...@comcast.net>>; Byron Weisz 
mailto:by...@cen-calfire.com>>; Michael de Gabriele 
mailto:mpdegabri...@gmail.com>>; Sprinkler Academy - C 
Bilbo mailto:prodesigngr...@msn.com>>
Cc: travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>; 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Velocity - Rant

Michael,
I would like to recommend NFPA 750 (Water Mist) for excellent information for 
your questioning.
Like Bob alluded to, H-W is not necessarily less accurate at high velocities. 
The variation from D-W comes from holding the C-Factor constant for all pipe 
size. This results in there being a particular velocity where D-W Pf starts to 
exceed H-W pf.
Since we are tied to H-W and constant C-Factor, technically this could be cause 
for concern regarding max velocity.
What is that particular velocity?
For 1” S40, H-W C=120, compared to D-W weight density= 62.34 lb/ft^3, dynamic 
viscosity= 1.1 centipoise, and absolute roughness= .002 inch, it is 40 ft/s. 
Since the particular velocity is higher (and different!) for larger pipe size, 
I would like to recommend 12 m/s as a self-imposed Speed Limit 

Intumescent Steel Protection (Not Sprinkler Question)

2019-02-14 Thread Bill Brooks
I apologize in advance for this question, and I invite off-line responses.  I 
also admit to not being 100% up-to-date on construction trends.  However, if 
there is a group who would be able to answer this it would be you.

 

I’m participating in a design for a 2 story office building with absolutely no 
special features, with the exception that the construction type is Type IIA.  I 
suggested using a gypsumboard membrane protection approach but the owner is 
steering the project to use of intumescent coating for steel structure, 
including bar joists – coatings shop-applied and touched up in the field after 
making connections.  I’ve been told this technique is becoming more prevalent.

 

Any feedback is welcome.

 

Bill Brooks

bill.bro...@brooksfpe.com

 

William N. Brooks, P.E.

Brooks Fire Protection Engineering Inc.

372 Wilett Drive

Severna Park, MD 21146-1904

410-544-3620

410-544-3032 FAX

412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Request for support

2017-05-09 Thread Bill Brooks
Rachid,

 

Use this link to access a worldwide network of Fire Protection Engineers.  They 
will be able to help you with your study and installation questions.

 

http://www.sfpe.org/?page=Chapters

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Rachid Saadaoui
Sent: Monday, May 08, 2017 5:42 PM
To: Sprinklerforum@lists.firesprinkler.org
Subject: Request for support

 

Hello

This is my first time working on the study and installation of a sprinkler 
system in a technical vacuum or there were cable tracks.

The dimensions of the technical voids are: L = 66.5m l = 7m and h = 4m.

Thank you to send me a free tool to do my hydraulic calculations, as well as 
determining number of head sprinkler

Best Regards

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ammunition Manufacturer

2017-01-21 Thread Bill Brooks
Instead of something being or not being your fight, why not say “I’ve never 
done anything like this before and I am not able to provide sprinkler design 
information for this specialized facility.  However, I am very capable of 
providing a sprinkler system layout for you when your registered design 
professional provides approved construction documents.”

 

In my opinion, this is one of the longstanding problems (challenges) with NFPA 
13.  It totally mixes work that should be performed by the design professional 
with the work performed by the sprinkler contractor.  It’s a recurring theme of 
many posts where the sprinkler contractor/designer is “solving” problems caused 
by failure to shift the design responsibility to a design professional.

 

Maybe it would be a good idea to add this concept to Chapter 1.  A design 
professional determines design criteria, a sprinkler contractor does system 
layout and calculations.  It’s probably too late for the 2022 edition and 
probably too radical an idea for the committee to consider.

 

Back to my resting mode.

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Friday, January 20, 2017 5:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Ammunition Manufacturer

 

They are disputing the F-1 Use Group. They contend that exception applies to 
big box stores like Dick’s Sporting Goods, not manufacturing. That’s not my 
fight, (I’m in over my head far enough as it is) I’m just trying to give the 
owner and whatever sprinkler contractor that I get involved, the right design 
criteria. 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ed Vining
Sent: Friday, January 20, 2017 5:10 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Re: Ammunition Manufacturer

 

​And have the State Plan Review people accepted the code review?

 

If the owner uses 200 pounds of propellant per day for a five day week, and if 
the code review limits are met, the owner is going to need two shipments per 
week. I'm sure the owner will feel this is burdensome.  Guess what!

 

On Fri, Jan 20, 2017 at 1:50 PM, John Paulsen <j...@crwnfire.com 
<mailto:j...@crwnfire.com> > wrote:

Uhh..no, it hasn’t worked that way in this case. It is a “rural” jurisdiction 
and the locals have been deferring to the State Plan Review people. (And I 
think rightfully so in this case.)

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> ] On Behalf Of Ed Vining
Sent: Friday, January 20, 2017 4:49 PM


To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Re: Ammunition Manufacturer

 

Has the AHJ bought into the code review?

 

On Fri, Jan 20, 2017 at 1:31 PM, John Paulsen <j...@crwnfire.com 
<mailto:j...@crwnfire.com> > wrote:

The plant machines need to have 200,000 primers and 200 lbs of powder available 
a day for manufacture. The verbiage below comes from the code review and has 
been agreed to by the owner.

 

Small Arms Primers

Quantities not exceeding 750,000 shall be permitted to be stored in a building 
where not more than 100,000 are stored in any one pile and where piles are at 
least 15 ft apart.

Small arms primers not stored in accordance with 14.5.6(1) through 14.5.6(2) 
shall be stored in a magazine meeting the requirements of Chapter 9. 

 

Smokeless Propellants

Quantities exceeding 100 Lbs, but not exceeding 800 Lbs, shall 
be stored in non-portable storage cabinets having walls of at least 1” 
thickness.

 

But again, in your all’s opinion, is this an Ex Haz Grp I or II, or something 
else? Just trying to figure out if I’m looking at the project the right way.

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438 <tel:(614)%20782-2438> 

F – 614-782-2374 <tel:(614)%20782-2374> 

C – 614-348-8206 <tel:(614)%20348-8206> 

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> ] On Behalf Of Charles 
Bamford
Sent: Friday, January 20, 2017 4:15 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Re: Ammunition Manufacturer

 

Paging Scott Mitchell..

 

On Friday, January 20, 2017 11:27 AM, "Hinson, Ryan" <rhin...@burnsmcd.com 
<mailto:rhin...@burnsmcd.com> > wrote:

 

How much DOT Class Division 1.1 (primer) and 1.3 (gunpowder)explosives will be 
located inside the building at any one time…and where?  What blast resistance 
requirements are required between said explosives and the rest of the building? 
  Where are explosives stored?  Have 

RE: Use of Set Screw Type Restraint Fire Pump Suction and Discharge

2016-12-19 Thread Bill Brooks
I appreciate the comments.  The body of my post describes the product (as 
presented on the cut sheet) as a wedge action restraint.  Probably should not 
have used the set screw language in the subject line – that shows my 
unfamiliarity with these products.  My concern is with the vibration associated 
with the diesel drive.

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of scott.mitch...@cns.doe.gov
Sent: Monday, December 19, 2016 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Use of Set Screw Type Restraint Fire Pump Suction and Discharge

 

Mr. Brooks appears to describe two differently designed products.  In his 
subject like he uses the words “Set Screw Type”.  But, in the body he describes 
a “wedge action restraint”. 

 

Some products use set screws to retain the pipe’s axial position in a flanged 
joint.  Some products use set screws for this same purpose in mechanical 
joints. The set screws exerts compressional or clamping force cutting a small 
pocket on the outer surface of the pipe wall. The screw tips are in shear when 
thrust bears on the joint.  This type of restraint can be successful at keeping 
the joint together when only exposed to internal pressure fluctuations. But, it 
is not suitable if the joint is exposed to vibrations such as is produced by a 
diesel engine driven fire pump.

 

The “wedge action restraint” appears to describe the design of products like 
Ebaa Iron’s Megalug or Romac’s RomaGrip.  The bolts are fitted with wedge teeth 
tips that penetrate the outer pipe wall.  Under load the teeth form a buttress 
of cold formed pipe material. As the load increases, the buttress increases 
transferring the load longitudinally along the pipe without affecting the 
design thickness of the pipe. These have been tested under severe cyclic loads 
and the wedge impressions look the same as if a single non-cyclical test had 
been performed.  If exposed to vibrations, it would appear that this design 
would perform better than the simple set screw; however, I don’t know if such 
testing has been conducted.

 

J. Scott Mitchell, PE

Senior Fire Protection Engineer

Mission Engineering

CNS Y-12 | 865-576-5258

CNS PTX | 806-477-5883

 


On Dec 16, 2016, at 6:20 AM, Bill Brooks <bill.bro...@brooksfpe.com 
<mailto:bill.bro...@brooksfpe.com> > wrote:

A case came up today about the use of a “mechanical joint wedge action 
restraint” on the suction and discharge side of a diesel driven pump.  Someone 
accepted a change and eliminated the rods, then put a MJWAC at the top of the 
ductile pipe on each side of the pump.  A commissioning agent has refused to 
start the pump based on the concern the restraint will “wiggle” off the end of 
the ductile under repeated pump operation either during the acceptance test or 
sometime later.

 

Is this a creative use of this type restraint, or is it a totally bad idea?  By 
the way, the underground elbow is a restrained type mechanical joint.

 

Thanks

 

Bill Brooks

Brooks Fire Protection Engineering Inc.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Use of Set Screw Type Restraint Fire Pump Suction and Discharge

2016-12-16 Thread Bill Brooks
A case came up today about the use of a “mechanical joint wedge action 
restraint” on the suction and discharge side of a diesel driven pump.  Someone 
accepted a change and eliminated the rods, then put a MJWAC at the top of the 
ductile pipe on each side of the pump.  A commissioning agent has refused to 
start the pump based on the concern the restraint will “wiggle” off the end of 
the ductile under repeated pump operation either during the acceptance test or 
sometime later.

 

Is this a creative use of this type restraint, or is it a totally bad idea?  By 
the way, the underground elbow is a restrained type mechanical joint.

 

Thanks

 

Bill Brooks

Brooks Fire Protection Engineering Inc.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: One weird cross connected system

2016-10-31 Thread Bill Brooks
Does this sound familiar??  I remember this from my days at GSA in the late
1970's.  It was presented by Mr. Meckler as a sprinkler system approach for
the old post office building in D.C. (currently Trump's hotel).  We rejected
the idea for a number of reasons - we couldn't figure out how it would save
money or work reliably.  Lots of moving parts.

 

Also incorporated into NFPA 13 at one point I think.  1985 edition,
"Automatic sprinkler systems with nonfire protection connections".

 

Bill Brooks

 

Patent number: 4286667

Abstract: Flow control and fire detection and location apparatus is
disclosed. The apparatus is used with a system which circulates heated or
cooled water for use in connection with the heating and air conditioning
system of a building and to sprinkler heads. The apparatus comprises a short
length of tubing or pipe connected downstream of a sprinkler connection to
provide a bypass for flow of heated or cooled water around a segment of the
return line from heating or cooling apparatus to a standpipe through which
the water is returned to an equipment room. There are check valves to
prevent flow of water through the bypass toward the heating or cooling
apparatus, and to prevent water flow in the bypassed segment from the
heating or cooling apparatus toward the standpipe. There is also a flow
sensor in the bypassed segment. In normal operation, water from the heating
or cooling apparatus flows through the bypass line to the standpipe and back
to the equipment room for heating or cooling and recirculation.

Type: Grant

Filed: February 27, 1979

Date of Patent: September 1, 1981

Assignee: Gershon Meckler Associates, P.C.

Inventors: Donald G. Westenhofer, Gershon Meckler

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Monday, October 31, 2016 6:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: One weird cross connected system

 

 
<https://tr.cloudmagic.com/h/v6/emailtag/tag/1477908647/2d4c4b9cd9f303a04c4d
9c24d32f6571/ecdd64c309bb34b23eb65c654267bfff/1fefe822716bbbd7efa6f3a027987f
92/9efab2399c7c560b34de477b9aa0a465/ufo.gif> 

I was at a location last Friday that had one of the strangest systems I have
seen. This is a 3 story office/retail space with underground parking
garages. The upper floors are wet and the garages dry. The sprinkler system
on the upper floor has several connections to feed mechanical equipment (VAV
boxes, etc.). This has been in place since the mid 1980s and the local AHJ
has made no comment. I'm sure this is not legal and I have no idea why they
do not get false alarms or why the fire pump does not go off on a regular
basis. Has anybody run into something like this before?

 

Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-608-4559 (cell)

 

via Newton Mail
<https://cloudmagic.com/k/d/mailapp?ct=ti=9.1.28=9.3.5=email_fo
oter_2> 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Drawing orders of hierarchy

2016-09-09 Thread Bill Brooks
What has the architect said about the design change?  You sprinklered based on 
a partial height wall and the drywall contractor built a full height wall?  And 
now you are being required to pay for his mistake?  I think your 
interpretation, especially given the “not connected” comment, is probably 
correct.  “Wall type” does not necessarily mean full height unless your set of 
drawings specifically call this out.  There are other details needed to show 
how a particular wall type is joined to a ceiling, floor, or other wall.  The 
Gypsum Construction Handbook is full of them.

 

http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=BXUV.U305
 
<http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=BXUV.U305=Fire-resistance+Ratings+-+ANSI/UL+263=1074330174=1073741824=versionless_id=1073984818=1>
 
=Fire-resistance+Ratings+-+ANSI/UL+263=1074330174=1073741824=versionless_id=1073984818=1

 

Take a look at this wall type from the UL Directory.  Nothing stated about 
partial or full height.

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ben Young
Sent: Thursday, September 08, 2016 11:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Drawing orders of hierarchy

 

Kind of strange, but does anyone know where I can find in writing somewhere 
some common sense info on the hierarchy of contract drawings?

Here's the issue:

Main floor print shows a particular wall as being 'type g' which is indicated 
as being full-height in the wall types plans.

Also shows the walls as not being 'connected' to the other walls it intersects 
with, which I know means its normally a different wall material, type, or some 
other indication of being 'not the same'

On the detail drawings for these areas, there's a note that says this 
particular wall is to only be 6'-6" in height and not going up to the deck.



GC is trying to claim that since the drywaller followed the overall plans, and 
we followed the detail plans, we're both equally at fault for this one.

I know that's ridiculous since just like dealing with codes, you can have a 
broad rule (wall type G) and then all specific exceptions to that rule on a 
case-by-case basis (a note saying this wall isn't full height) 

Similar to a note that says 'all walls to be full height unless indicated 
otherwise.'

I'm pretty comfortable defending my position, especially since the overall 
floor plans have a note to reference the detail drawings.

FYI, this is a hotel, and the main floor plans don't show the notes, but the 
unit plans (plan, finish, interior elevations, etc) do.

I'm just wondering if there's some obscure AIA document that says how this is 
supposed to work, or anything I can fall back on besides common sense, which we 
all know doesn't exist inside most superintendent's offices on construction 
projects.

For the record, I showed the walls dashed on my plans which indicates a wall 
that doesn't cross the RCP cut plane, and there's a counter in the room which 
has the same dashed linetype.  Both were not indicated as dashed on the 
architectural plans, so I changed them on my RCPs for submittal based on the 
notes on the unit drawings.

Yes, this involves a change order over added heads.

There's nothing in the specs or drawings that I can definitively point to that 
says what I'm looking for, so this is a last ditch effort.

Also, my plans have already been approved by the A/E team, and the AHJ.  We 
only noticed this when we saw the wall framing going up to the ceiling on-site.

Any help would be greatly appreciated.

Thanks,

Ben


Benjamin Young

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flexheads in small renovation (Calculation Software)

2016-08-30 Thread Bill Brooks
You will be able to tell this question is based on minimum software application 
experience, but does current software automatically determine “most demanding”? 
 Or, is it up to the human operator to guess where this area might be?  If it’s 
a guess, how do you know you have chosen correctly?

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Tuesday, August 30, 2016 10:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flexheads in small renovation

 

To underscore John’s point, these fittings impose with a SUBSTANTIAL pressure 
loss.   As 3rd party, we would ask for calculations to prove the performance of 
the revised configuration.

 

SL

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Michael Hill
Sent: Tuesday, August 30, 2016 6:11 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Flexheads in small renovation

 

I agree with Richard, it needs to be evaluated. It is known that flex piping is 
generally more demanding than their hard piped counterparts. If the base 
building design did not include flex piping, I would look at it as a change to 
base building design and perform a quick calculation to see how it looks. I 
assume they didn’t use excessively long flex pipe with more bends or lops than 
were needed.

 

Mike Hill

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Tuesday, August 30, 2016 8:39 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Flexheads in small renovation

 

This is a single story building. Multiple looped 4" and 3" cross mains with 
branches to wings. (Think nursing home with interior court yards). No fire 
pump. 100 psi static with a flat curve (2 year old test, DeltaE = 0). Area in 
question not most hydraulically remote but toward that end of the building. 
Branch lines are fed from the loop, not a DE branch main. LH occupancy. 

 

I am not worried about this not being adequate, more a consensus of what needs 
to be done and what is correct. 

Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-608-4559 (cell)

 

Sent using CloudMagic 
<https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2> 

 

On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr <rc...@coxfire.com 
<mailto:rc...@coxfire.com> > wrote:

I can’t disagree with John (Hi John) but we need more info to make the call,

In remote area?

Fire pump?

What is safety margin on existing?

What is friction loss on the flex?

 

Just because you add 4 flex piping to an existing system does not require it to 
be calculated. But does need to be evaluated.

 

Richard Carr, SET

Branch Manager

Cox Fire Protection, Inc

6555 Grace Lane.

Jacksonville, Fl. 32205

rc...@coxfire.com <mailto:rc...@coxfire.com> 

904-781-8227

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: Tuesday, August 30, 2016 7:14 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Flexheads in small renovation

 

I disagree with Richard. (Hi Richard!)

 

Relocating these sprinklers with flex heads may very well change the location 
of the most hydraulically remote area to the place you are working. Flex-heads 
come with a substantial pressure loss. Even if doing calculations wasn’t 
required, I would want to do them for myself for peace of mind. My belief has 
always been that you can’t tax the system without verifying that it still works.

 

John Irwin

Manger – Fire Sprinkler Division

Critical System Solutions, LLC
Cell: 813.618.2781

Email:  jir...@criticalsystemsolutions.com 
<mailto:jir...@criticalsystemsolutions.com> 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Carr
Sent: Tuesday, August 30, 2016 7:08 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Flexheads in small renovation

 

Are the relocates in the remote area? if not I would not calc. also , some flex 
brands are better that others as far as friction loss.

 

Richard Carr, SET

Branch Manager

Cox Fire Protection, Inc

6555 Grace Lane.

Jacksonville, Fl. 32205

rc...@coxfire.com <mailto:rc...@coxfire.com> 

904-781-8227

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Tuesday, August 30, 2016 6:30 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Flexheads in small renovation

 

I have a client that did a 4 sprinkler relocate job in an office and used 
Flexheads (no sprinklers added

RE: Separation of Fire Mains from other utilities

2016-08-23 Thread Bill Brooks
Military projects may bring in other requirements by referencing various UFC
for example.

 

Bill Brooks

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Morey, Mike
Sent: Tuesday, August 23, 2016 8:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Separation of Fire Mains from other utilities

 

I thoroughly reviewed NFPA 24 and reviewed the applicable chapters of
IFC/IBC slightly less thoroughly, and I can't find any guidance there.  Is
there any code or standard, AWWA etc that might give some guidance on
minimum separation from other utilities?

 

Mike Morey, CFPS, SET

Planner Scheduler/Designer

BMWC Constructors, Inc.

1740 W. Michigan St, Indianapolis, IN 46222

O: 317.651.0596 | C: 317.586.8111
 
<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXh
x81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.=mailto%3amanta%40bmwc.com>
mo...@bmwc.com |
<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXh
x81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.=http%3a%2f%2fwww.bmwc.com%2f>
www.bmwc.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Existing pipe schedule and storage

2016-04-27 Thread Bill Brooks
As a PE you would be remiss in not noting your concerns.  However, it
appears the owner is relying on his/her insurance entity and the AHJ for the
current risk assessment.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 8:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Existing pipe schedule and storage

Actually this is part of the pre 1896 pipe schedule system I mentioned in
previous posts. The branch line sizing is less that the 1896 standards. No
major renovation >20%. Density requirements would be approx .24/2000.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Wed, Apr 27, 2016 at 8:31 AM, John Paulsen <j...@crwnfire.com> wrote:
Todd:

I have come across this situation a couple of times and in my experience,
you are waltzing in a mine field.
I am going to assume for the sake of argument that:
The existing pipe scheduled system is per the OLD Extra Hazard pipe
scheduled guidelines.
The Class IV storage usage is a change from the building's original use.
And that the building has not undergone a > 20% area renovation recently.
The commodity being stored would normally require the overhead system to
meet a design density consistent with an Extra Hazard demand.

NFPA 13, 23.5 relegates pipe scheduled systems to only being acceptable as
an existing situation and in my experience, any major change in use is an
excuse to prove it hydraulically and 23.5.4 states that all Extra Hazard
systems must be hydraulically calculated. However the part of your email
that states the AHJ has approved it, tells me that you could be picking the
wrong fight. You could do a quick calculation and show the existing system
to be woefully inadequate, then inform the owner and fire prevention. At
least you would have documentation that you brought it to their attention in
the event of a fire.

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206





-Original Message-
 From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 6:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Existing pipe schedule and storage

I am working at a facility where there is an existing OH pipe schedule
system over 12ft palletized Class IV storage. The fire department has
approved it, but I question whether it will provide adequate protection. I
did not see anything in NFPA 13 that requires storage occupancies to be
hydraulically calculated. Am I missing something?
This is outside of the project I am working on, but as an FPE, I feel
obligated to notify someone if I see a potential hazard such as this.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Existing pipe schedule and storage

2016-04-27 Thread Bill Brooks
Palletized probably better than rack.  Class IV probably better than Group
A.  OH better than LH.  Wet probably better than dry.  Pipe schedule
probably better than no system.  Water flow reported to a supervising
station better than cell phone from highway.

The 1973 edition of NFPA 13 had an OH3 category which included warehouses.
Water supply was at the discretion of the AHJ although a hydraulically
calculated system at the time required 750 gpm.

Bill Brooks



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 6:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Existing pipe schedule and storage

I am working at a facility where there is an existing OH pipe schedule
system over 12ft palletized Class IV storage. The fire department has
approved it, but I question whether it will provide adequate protection. I
did not see anything in NFPA 13 that requires storage occupancies to be
hydraulically calculated. Am I missing something?
This is outside of the project I am working on, but as an FPE, I feel
obligated to notify someone if I see a potential hazard such as this.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipe Calc: Adding City Demand to Pumper Truck?

2016-03-22 Thread Bill Brooks
And sometimes the hose used to connect the pumper to the FDC is an issue as
well if it is not rated for higher pressures.

I know this is something we toss back a forth but shouldn't the Engineer of
Record be the person to do this legwork ahead of time?

Bill Brooks
Brooks Fire Protection Engineering

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Tuesday, March 22, 2016 12:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Standpipe Calc: Adding City Demand to Pumper Truck?

Attention Everybody (and Sean):

It is time for us as an industry to move outside the box.   Prescriptive
codes and standards are convenient, and most AHJ's will defer to them
without amendment or interpretation because it's usually not required to do
so.   But sometimes we have to address situations that ARE subjective and
this is one of those - you have to meet with the serving fire department to
verify their operational practices and pumping capabilities.  Your statement
that the pumper is "... sized for 150psi at 1000gpm" isn't accurate;
generally, modern pumpers and engines can make up to 300 PSI at either 1,000
or 1,500 GPM so available pressure isn't the issue.  Design of the system
and identification of the demand are the issues.150 PSI is an industry
practice, not an absolute threshold that can't be crossed and NFPA 14 has a
requirement that you must hang a sign on the FDC informing the FD of the
required pressure to meet the calculated demand.   

As with sprinkler systems, Pressure = $$, so the more you have the smaller
the piping can generally be and you save $$.   150 is a safe starting
pressure so most FD's will require that you use that as a source pressure;
if a manual standpipe system is a little longer or taller and requires more
pressure we can make that up by subbing 6" for 4" and it still works at 150.
But in taller buildings, you will need more pressure so, if you want to do a
70' tall building  with 4" risers all the way up the shafts, then you have
to obtain FD approval to pump at 195 or 215 or whatever it turns out to be.
And, you have to build the system out of components rated for that pressure,
which is actually no big deal these days.And when it's over, you badge
the FDC with a sign that states, "PUMP 1000 GPM AT 215 PSI TO MEET DEMAND AT
STAIR #2 ROOF" or something like that (your FD will tell you how to word the
sign). 

Partner up people ...

The preceding is my opinion only and does not represent the opinion of or an
interpretation of the standard by NFPA or the Technical Committee on
Standpipes.

Steve L.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of svang...@aerofire.com
Sent: Tuesday, March 22, 2016 8:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Standpipe Calc: Adding City Demand to Pumper Truck?

Sorry for coming into this a week late.  We have recently been dealing with
specs and AHJ requirements that state we need to supply 130psi and/or 140psi
at the top outlet regardless of whether it is manual or automatic.  Same
flows as outlined in NFPA 14 (500gpm +250gpm per standpipe up to 1000gpm).
The fire pumper truck is still sized for 150psi @ 1000gpm.  What do you
suggest we do if we can only set the FDC to be the source of 151@0 and
150@1000?  Some building are still 70ft tall and the standpipe is still a
manual wet.  Only accounting for elevation we are looking at 160psi/170psi
demand at the FDC.  Even if your answer is make it an automatic standpipe,
the 140psi requirement limits the "manual" standpipe building height to 23ft
when we don't account for friction loss using your calculation procedure.
So we can't even meet these manual FDC 150psi calcs on a building that
doesn't even need a standpipe.

Thanks,
Sean VG



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Monday, March 14, 2016 3:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Standpipe Calc: Adding City Demand to Pumper Truck?

Tony:

You (or the submitter) are over-simplifying what the annex says.  It's not
the intent that you take the city flow test and add it to the pumper curve.
NFPA 1901 sets the basic performance curve for a pumper at 150 PSI/1,000
GPM.   NFPA 13E is the standard for FD Operations for buildings equipped
with sprinklers and standpipes - that standard goes into the company
engineer's procedure for calculating the discharge pressure of the pump
based on suction pressure, friction loss in hose and other variables.   But
the bottom line is that it's all targeted at discharging 150 PSI residual at
1,000 GPM.   This has NOTHING to do with pressure at the FDC; it has to do
with calculating the performance of the apparatus.   What gets to the FDC is
up to the engineer.

Which

RE: Preaction Systems Scope

2016-02-09 Thread Bill Brooks
It's nice to know, after more than 40 years at this stuff, we still have the
same coordination issues.  I thought these problems could be fixed with
smart phones and snapchatting.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rongreenman .
Sent: Tuesday, February 09, 2016 4:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Preaction Systems Scope

The problem of nobody bidding the detection, but everybody excluding it, was
exactlty what happened at the C-17 Simulator building at McChord AFB.


On Tue, Feb 9, 2016 at 12:04 PM, <craig.pr...@ch2m.com> wrote:

> Price is all they care about.
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> craig.pr...@ch2m.com
>
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Michael 
> Hill
> Sent: Tuesday, February 09, 2016 2:55 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Preaction Systems Scope
>
> Can you send those contractors our way. We can cloud, highlight and 
> put arrows pointing to our exclusions and the general contractor still 
> only sees the price at the bottom of the page.
>
> Mike Hill
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of rongreenman .
> Sent: Tuesday, February 09, 2016 2:05 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Preaction Systems Scope
>
> You could have a base bid price excluding the electrics, with an "in bold"
> extra for the inclusion electrics. That might get their attention and 
> still let them compare apples to apples. I know I've done that and 
> that started someone asking questions about just what the other bids
included.
>
> On Tue, Feb 9, 2016 at 11:00 AM, Rod DiBona <r...@rapidfireinc.com> wrote:
>
> > Thank you all for your help. That is what I thought but we were 
> > starting to wonder if we were the only ones that seem to 
> > consistently have this problem. We so clearly, in bold exclude it in 
> > detail and then still end up with a fight at the end because the GC 
> > didn't buy it out. We were considering just including all of it in 
> > all of our preaction bids so they get a complete system and 
> > eliminate the hassle but felt that this would make us less 
> > competitive if others weren't doing the same. We will continue to 
> > exclude and see if we can't find a better way to communicate that 
> > this is a likely scope gap unless it is
> addressed at bid time.
> >
> > -Original Message-
> > From: Sprinklerforum [mailto:
> > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> rongreenman .
> > Sent: Tuesday, February 09, 2016 11:03 AM
> > To: sprinklerforum@lists.firesprinkler.org
> > Subject: Re: Preaction Systems Scope
> >
> > Here it is typically handled like Mike describes too. Everyone 
> > pretty much knows the general's contracts guy will miss all the 
> > exclusion clauses unless he's been bitten before. The object is to 
> > get the building built with all systems working.
> >
> > On Tue, Feb 9, 2016 at 9:53 AM, Morey, Mike <mo...@bmwc.com> wrote:
> >
> > > Typically we tried to let the project team work it out, but if 
> > > they didn't or there wasn't a well defined project team to resolve 
> > > these issues we'd typically take it out for numbers.  Usually we 
> > > try and get the electrical/alarm bidders for the project to put a
number on it.
> > >
> > > Mike Morey, CFPS, SET
> > > Planner Scheduler/Designer
> > > BMWC Constructors, Inc.
> > > 1740 W. Michigan St, Indianapolis, IN 46222
> > > O: 317.651.0596 | C: 317.586.8111
> > > mo...@bmwc.com | www.bmwc.com
> > >
> > > 
> > > From: Sprinklerforum
> > > <sprinklerforum-boun...@lists.firesprinkler.org>
> > > on behalf of Rod DiBona <r...@rapidfireinc.com>
> > > Sent: Tuesday, February 9, 2016 12:25 PM
> > > To: sprinklerforum@lists.firesprinkler.org
> > > Subject: Preaction Systems Scope
> > >
> > > I am wondering how most of you handle the detection and releasing 
> > > systems for your preaction systems. We traditionally have excluded 
> > > all 

RE: Locker Rooms (who prepared the Owner's Certificate)

2016-01-05 Thread Bill Brooks
What about the Owner's Certificate required by 4.3 in the 2007 edition and
for all editions since then?  Has anyone checked this document to see what
the declared use of the space is?  Why does the sprinkler contractor always
seem to take on the responsibilities of others?

There's also the language of 1.2.1 (2007) with regard to "reasonable degree
of protection for life and property".  It doesn't say the sprinkler system
will forever be perfectly matched up with the contents under it.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Tuesday, January 05, 2016 12:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms

And my comments were in tacit support of your perspective, based on
historical performance.   You are much more in touch with what the good
people of Lake Oswego are going to do (or not) in those situations.   The
challenge for an industry that still delivers 90+%  of its designs on a
deferred basis is to determine what's actually required before starting
preparation of plans, so all we would ask is that if you want it, codify it
or advise the ownership team of those requirements in the earliest possible
phases of the project.  

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Smith, David
Sent: Tuesday, January 05, 2016 9:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms

I understand (& support) your perspectives and was simply trying to answer
Todd's question of what could be stored in a locker room; based on my
experiences. Hopefully during the plan review process, the AHJ is able to
look at these locations (& location on site; next to the track) and make
appropriate comments back regarding these potentials. I am by no means
supporting a situation where a local AHJ simply says to change it.

I would prefer asking the questions or pointing out where meeting minimum
code requirement could potentially cause a future problem during the review
process where it then gets documented within the comments. Particularly when
some years later that documentation resurfaces as part of the explanation as
to why they can't do what they are doing and are limited to the original
design or make necessary upgrades.

David Smith | Deputy Fire Marshal
P 503.635.0378 | F 503.635.0376
dsm...@ci.oswego.or.us
300 B Avenue | PO BOX 369 Lake Oswego OR 97034


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Tuesday, January 05, 2016 8:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms

Valid point for an engineer of record to ponder during the A/E design.  But
if nothing is stated to a bidding contractor other than the space will be
locker rooms, than nothing should be inferred other than a standard, light
hazard, locker room space.

Contractors should not be obligated to extrapolate occupancy classifications
to anything beyond that described on the plans, unless it has been codified
or otherwise declared in the bidding documents.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Smith, David
Sent: Tuesday, January 5, 2016 10:01 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Locker Rooms

I have seen portions of locker rooms sectioned off with chain link fencing
material and plywood walls for security and used to store all kinds of
things. Items can include various sporting equipment; large piles (~1200 sq
feet and 8 feet tall) of rubber mats used for track high jump mats, tackling
dummies, wrestling mats, stacks of plastic cones, piles of plastic street
hockey sticks, foam dodge balls, portable plastic bleachers, stacks of
folding plastic tables, gymnastic mats, or the best one chemicals for the
chemistry class.

These rooms evolve over time and in a number of schools, they no longer use
the locker rooms resulting in them being sectioned off as storage areas; or
even used as office space.

I'm not saying it's necessary to go to OH1 but it's often easier to have it
built that way during construction than having to re-educate every new
principal, PE teacher or building engineer for the life of the building when
inspections are done what can/can't be in these spaces. Worse is having them
go back and modify the system if they do change the use of an area over
time.

David Smith | Deputy Fire Marshal
P 503.635.0378 | F 503.635.0376
dsm...@ci.oswego.or.us
300 B Avenue | PO BOX 369 Lake Oswego OR 97034

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Wil

RE: Locker Rooms (who prepared the Owner's Certificate)

2016-01-05 Thread Bill Brooks
So it would seem that the "sprinkler installer" would have some sort of
QA/QC checklist with things on it like:
1. Address of Building
2. Owner's Certificate
3. Water supply quality information

That's it for me on this.  Seems things an owner is required to do should be
in the building or fire code, and things the sprinkler contractor should do
should be in NFPA 13.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Tuesday, January 05, 2016 3:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Locker Rooms (who prepared the Owner's Certificate)

I believe the language in 13 says the Owner's Certificate should (not
shall) be
used. It is also in 2002 and I have never seem one.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Tue, Jan 5, 2016 at 3:14 PM, sprinklerforum@lists.firesprinkler.org
<sprinklerforum@lists.firesprinkler.org> wrote:
"What about the Owner's Certificate required by 4.3 in the 2007 edition and
for all editions since then? Has anyone checked this document to see what
the declared use of the space is? Why does the sprinkler contractor always
seem to take on the responsibilities of others?"

Because - at least in the case of projects with A/E teams - the engineers
are rarely held to account for their efforts. I would venture guess that a
large percentage of engineering firms being paid for their 'performance
specifications' haven't the foggiest clue about what we're talking about in
this thread. To them a good contractor is one that has few change orders,
gets to the job on time, and makes few waves. The fact that they've dumped
design authority onto that same low-bid contractor is completely missed or
ignored.
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Healthclub on top of parking structure

2015-04-14 Thread Bill Brooks
There's also 2012 IBC 903.2.11.3 referring to buildings = 55 ft.  Been in 
there since at least 2000 edition I believe.

Bill Brooks
AFSA Member

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Tuesday, April 14, 2015 12:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Healthclub on top of parking structure

And that is because ...?   





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Joe
Sent: Tuesday, April 14, 2015 9:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Healthclub on top of parking structure

To be clear - this is high-rise by IFC standards.
?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ignoring new standard requirements

2015-04-03 Thread Bill Brooks
So a corollary would be - do you declare your previous jobs to be unsafe or
somehow not acceptable if a new code or standard is published?  Do you
notify your previous customers about this? Somehow I think you don't.  All
in all, designing in accordance with adopted codes and standards is a
defensible standard of care in my opinion.  Otherwise, where do you go to
search out the safest code approach?  Another city, another state, another
country?

Bill Brooks
AFSA Member

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of svang...@aerofire.com
Sent: Friday, April 03, 2015 12:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ignoring new standard requirements 

Thank you all for your response and input.

Mark hit the nail on the head for what I was driving at regarding the PE's
obligation to society, and how one would deal with this kind of problem.  If
I'm not mistaken, your code of conduct requires you to lookout for welfare
and safety of society.  You can only do that by basing your design on the
most current information.  But if an AHJ doesn't require the newest codes,
whether more stringent or less as many have pointed out, then as a
subcontractor you may be pricing yourself out of a competitive bid.  So you
are stuck with the dilemma...meet the code of conduct, or ignore the latest
requirements to compete with other subcontractors so you can put food on
your plate.

Going all dramatic here...but which is the lesser of two evils.  Has anyone
heard of a legal case involving this type of scenario and what the outcome
was?  

      Thanks,

Sean Van Gaal

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Friday, April 03, 2015 8:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ignoring new standard requirements 

My favorite example of this conundrum goes back to the transition to the
requirement in 13 for the use of QR sprinklers in Light Hazard, and the
reduction in design area allowed by their use.  I believe this occurred in
the '96 edition - whatever, our local codes were following earlier editions
of 13.  So when the engineer specifies to design to the latest edition of
NFPA 13 and follow state and local codes, what do you do? QR sprinklers at
the time were more expensive; but you could get the reduced design area,
which could save money. Meanwhile, since the most recent edition of 13
called for their use, it was implied that QR was superior protection to
standard response in Light Hazard occupancies.

Galen's response make the most sense, but in my example, we were a
contractor competing for a job as a sub-contractor to mechanical - or maybe
sub- to a sub- of the general. No one cared about such an issue during
bidding. If you won the job, no one was going to listen to your esoteric
discussion about the benefits of QR sprinklers unless you were willing to
give a deduct change order. It was more difficult after receiving my PE,
when I became professionally obligated (not just morally) to provide the
best system for our customer.

The QR issue was relatively minor and I am certain no one suffered injury
because our local codes didn't adopt the latest version of 13 at that time.
But it highlights the challenge and emphasizes a common point on this forum:
engineers of record need to be more engaged in and take more responsibility
for the fire suppression aspect of their job. And if the opportunity is
available to contractors (with or without PEs on staff), they should take
Galen's advice and propose alternative designs based on the latest
standards.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of svang...@aerofire.com
Sent: Thursday, April 02, 2015 7:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: ignoring new standard requirements

I'm sorry for my grammar and autocorrect as this is coming from my phone.

How does the forum feel about ignoring the more stringent requirements of
the most current NFPA standards all because the AHJ hasn't adopted the
latest year?  As the standards have evolved with each new addition, they
typically try to clarify murky wording of past standards, expand on topics,
or add/change requirements based on the latest and greatest tests.  So
should we be purposely designing and installing and inferior product that
more times than not is less safe just because the AHJ hasn't adopted the
latest design guidelines.  I've heard sometimes the AHJ doesn't adopt the
new standard simply due to the financial impact of republishing their
amendments and not merely because they don't agree.  To me it seems
morally/ethically wrong

Fire Wall Integrity

2015-03-26 Thread Bill Brooks
John, now that you bring up the subject of collapse on both sides, just how
do you treat this subject?  I have seen the interpretation which appears to
suggest that a sprinkler pipe penetration of a fire wall would not be
acceptable if the pipe (in coming down with collapsing side) somehow
compromised the gypsumboard separation assembly.  Same with an electrical
conduit.  I'm also not sure how to design the collapsing side in such a way
that it falls cleanly to the ground without some member shifting sideways
and penetrating the separating assembly.

In other words, do you wait till after the fire to say it works or doesn't
work?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Drucker
Sent: Wednesday, March 25, 2015 6:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Floor Control Stations

LOL Horizontal Fire Wall..we inspectors are still scratching our heads
how this meets the performance definition of a firewall...collapse on one
side, stays in placethen again sprinkler guys are famous for skyhooks.
You just can't make this stuff up.

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823


rongreenman . rongreen...@gmail.com wrote:

Roland,

Would you think with all the hoopla about non-combustible floor assemblies
being equivalent to horizontal fire walls. and high rises typically not
needing vertical fire separation, that a floor would fit a loose definition
of a zone? Two floors, even if within the area limits of a single system
seem to define two zones. Just thinking, and remember that Leyton was
concerned this morning that my meds have lost their efficacy, so I may just
be having another flashback to the sixties.


On Tue, Mar 24, 2015 at 12:00 PM, David Blackwell 
david.blackw...@llr.sc.gov wrote:

 On a related note and of interest to this forum should be the change 
 to next section, IFC 914.3.1.2, in the 2015 edition.  The limiting 
 phrase In buildings that are more than 420 feet (128m) in building 
 height, has been added to the 2015 edition published by ICC.  Prior 
 to that change, the 2012 edition applied the separate supply piping 
 requirement per IFC 914.3.1.2 more broadly to include high-rise buildings
below that height.

 Respectfully,


 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation, 
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/


 Please note that you can sign up to receive automatic information on SC
 Division of Fire and Life Safety current events, policies, laws and
 procedures by visiting our Web site at:
 http://www.scfiremarshal.llronline.com/


 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland
 Huggins
 Sent: Tuesday, March 24, 2015 2:45 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Floor Control Stations

 The main point is that for standard high rises, the codes and standards
 only require a single riser.

 Very Tall High Rises (420 ft) are a unique beast.  The IFC requires these
 tall buildings to have 2 risers per zone.  Not 100% sure but I don't think
 they mean each floor is a zone.  The same section says Each riser shall
 supply sprinklers on alternate floors.  A lot of these building going up
 in parts of the Middle East but not hearing about any here in the USA.
Any
 one involved with one?

 Roland


 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org http://www.firesprinkler.org/





  On Mar 20, 2015, at 9:55 AM, David Blackwell
david.blackw...@llr.sc.gov
 wrote:
 
  It is also found in Section 914.3.1.1 of the 2012 IFC, which is
 referenced from 2012 IFC Table 903.2.11.6 [Additional Required Fire
 Suppression Systems].
 
  Respectfully,
 
 
  David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of
  State Fire Marshal SC Department of Labor, Licensing,  Regulation,
  141 Monticello Trail, Columbia, SC 29203
  Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
  Fax: 803.896.9806 [Office]
  Email:   david.blackw...@llr.sc.gov
  Website:  http://www.scfiremarshal.llronline.com/
 
 
  Please note that you can sign up to receive automatic information on
  SC Division of Fire and Life Safety current events, policies, laws and
  procedures by visiting our Web site at:
  http://www.scfiremarshal.llronline.com/
 
  -Original Message-
  From: Sprinklerforum
  [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
  Fairchild, Jack
  Sent: Friday, March 20, 2015 12:15 PM
  To: sprinklerforum@lists.firesprinkler.org
  Subject: RE: Floor

RE: Fire Wall Integrity

2015-03-26 Thread Bill Brooks
Yes, I am aware of this.  But it is possible to create a fire wall with
gypsumboard, and this is where the collapse on both sides without damaging
the wall comes into play.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of craig.pr...@ch2m.com
Sent: Thursday, March 26, 2015 3:25 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Wall Integrity

There are physical differences and penetration restrictions based on whether
the membrane is a Fire Wall or Fire Partition or other codified separation.


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Bill Brooks
Sent: Thursday, March 26, 2015 3:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Wall Integrity

John, now that you bring up the subject of collapse on both sides, just how
do you treat this subject?  I have seen the interpretation which appears to
suggest that a sprinkler pipe penetration of a fire wall would not be
acceptable if the pipe (in coming down with collapsing side) somehow
compromised the gypsumboard separation assembly.  Same with an electrical
conduit.  I'm also not sure how to design the collapsing side in such a way
that it falls cleanly to the ground without some member shifting sideways
and penetrating the separating assembly.

In other words, do you wait till after the fire to say it works or doesn't
work?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Drucker
Sent: Wednesday, March 25, 2015 6:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Floor Control Stations

LOL Horizontal Fire Wall..we inspectors are still scratching our heads
how this meets the performance definition of a firewall...collapse on one
side, stays in placethen again sprinkler guys are famous for skyhooks.
You just can't make this stuff up.

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823


rongreenman . rongreen...@gmail.com wrote:

Roland,

Would you think with all the hoopla about non-combustible floor assemblies
being equivalent to horizontal fire walls. and high rises typically not
needing vertical fire separation, that a floor would fit a loose definition
of a zone? Two floors, even if within the area limits of a single system
seem to define two zones. Just thinking, and remember that Leyton was
concerned this morning that my meds have lost their efficacy, so I may just
be having another flashback to the sixties.


On Tue, Mar 24, 2015 at 12:00 PM, David Blackwell 
david.blackw...@llr.sc.gov wrote:

 On a related note and of interest to this forum should be the change 
 to next section, IFC 914.3.1.2, in the 2015 edition.  The limiting 
 phrase In buildings that are more than 420 feet (128m) in building 
 height, has been added to the 2015 edition published by ICC.  Prior 
 to that change, the 2012 edition applied the separate supply piping 
 requirement per IFC 914.3.1.2 more broadly to include high-rise 
 buildings
below that height.

 Respectfully,


 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation,
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/


 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:
 http://www.scfiremarshal.llronline.com/


 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland 
 Huggins
 Sent: Tuesday, March 24, 2015 2:45 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Floor Control Stations

 The main point is that for standard high rises, the codes and 
 standards only require a single riser.

 Very Tall High Rises (420 ft) are a unique beast.  The IFC requires 
 these tall buildings to have 2 risers per zone.  Not 100% sure but I 
 don't think they mean each floor is a zone.  The same section says 
 Each riser shall supply sprinklers on alternate floors.  A lot of 
 these building going up in parts of the Middle East but not hearing about
any here in the USA.
Any
 one involved with one?

 Roland


 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org http://www.firesprinkler.org/





  On Mar 20, 2015, at 9:55 AM, David Blackwell
david.blackw

RE: Underground Piping Under Slab

2015-02-20 Thread Bill Brooks
Highly desirable is an understatement I assume?  I'm just hoping this is a
typographical thing.  I sent an email to NFPA earlier this week on this - no
response yet.  So many more things could be done to make the online
subscription more useful like having errata noted and having TIAs noted and
linking all text changes directly to the ROP/ROC or whatever these are
called now and maybe more.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Friday, February 20, 2015 3:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Underground Piping Under Slab

NFPA has at least temporarily stopped flagging the sections that have
changed.  Not sure how long this will continue.  IT has been expressed
pretty loudly that having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov
wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and
handbook, I noticed that while the language of 10.6.3.1 has changed in the
2013 edition to clarify the 10 ft distance, but the section was not marked
as new in either the printed code, the handbook or the PDF version available
through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation, 
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.)
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire
service mains enter under the building no more than 10 ft (3 m) as measured
from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 
 categorically states not to do something, yet 10.6.2 allows it.  
 Elimination of 10.6.1 seems the thing to do and would not change the 
 intent.  After all it's impossible to meet 10.6.1 unless you put the 
 stub up in an exterior enclosure and route it through the exterior 
 wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too
much?
 
 If this is important it should be submitted as a Building, Plumbing,
Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to
say what you really meant was that as long as the plumbing inspector is OK
with the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building 
 slab but if it's a must there are some precautions that must be taken 
 as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned
all required or as a bare minimum? I'm working on a project and the
architect has located the riser room in the center of the building,
approximately 15'
 from the outside wall. I brought it to their attention that it's not the
best idea and provided them the above code reference. Instead of
appreciating the heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http

RE: Underground Piping Under Slab

2015-02-13 Thread Bill Brooks
The new NFPA exception formatting is interesting.  10.6.1 categorically
states not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1
seems the thing to do and would not change the intent.  After all it's
impossible to meet 10.6.1 unless you put the stub up in an exterior
enclosure and route it through the exterior wall.  Even the language in
10.6.3 is an exception to 10.6.1.  How much inside the building is too much?

If this is important it should be submitted as a Building, Plumbing,
Mechanical Code change and removed from NFPA 13.

So, like we see on TV, you should now clarify your meeting comments to say
what you really meant was that as long as the plumbing inspector is OK with
the special precautions so are you.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, February 12, 2015 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab
but if it's a must there are some precautions that must be taken as shown in
10.6.2 (2007). My question is are the (3) provisions that are mentioned all
required or as a bare minimum? I'm working on a project and the architect
has located the riser room in the center of the building, approximately 15'
from the outside wall. I brought it to their attention that it's not the
best idea and provided them the above code reference. Instead of
appreciating the heads up I'm now the redheaded step child, go figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Relocate sprinklers with drops RETORT (resend)

2015-02-07 Thread Bill Brooks
Sorry, it appears only the dry type can be replaced, but it still looks like
you can remove the drop (including the head) and replace it.  I thought I
saw an exception for flex heads too.  Maybe this could be clarified further.


So sprinklers removed for NFPA 25 inspection procedures and dry sprinklers
can be replaced, but other sprinklers can't?  Even though the same people
are handling all of them?  I don't see how these exceptions make sense.  I'm
pretty much old school on most things but what would allow ANY sprinkler to
be replaced given the bucket of heads argument?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Cahill, Christopher
Sent: Saturday, February 07, 2015 11:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Relocate sprinklers with drops RETORT

Agree - here's my question where's the data or experience this is a problem?
For 15 years I was either the FPE for St. Paul or a sprinkler contractor.
In St. Paul I personally went to about 90% of the sprinkler activations and
as a contractor we were small enough I knew of everything we did.  Not once
did I have any reason to believe a false discharge was caused by a
repositioned head whether removed from it's fitting or not.  I have to
believe there were 10's of thousands of heads moved in this period.

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Greg McGahan
Sent: Friday, February 06, 2015 8:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Relocate sprinklers with drops RETORT

It sure seems like a waste of resources to me. 

Sent from my iPhone

 On Feb 6, 2015, at 6:49 PM, rfletc...@aerofire.com
rfletc...@aerofire.com wrote:
 
 Like shipping, unpacking and installation only applies the proper and
necessary stress for the sprinkler to operate as intended. Or maybe the
engineering is so precise that the sprinkler can only stand the rigors of
being threaded into a fitting once and then it's useless. Or maybe there are
sprinkler manufacturers reps on the 13 committee that know how fragile and
un-robust sprinklers are? Why would you build something could only be
threaded in once? I'm glad they don't manufacture pipe or fittings.
 
 Ron fletcher Sent from my iPhone
 
 On Feb 6, 2015, at 4:43 PM, John Denhardt jdenha...@stricklandfire.com
wrote:
 
 Mark - well said. I totally agree. 
 
 Sent from my iPhone
 
 On Feb 6, 2015, at 6:29 PM, Mark A. Sornsin, P.E.
masorn...@kfi-eng.com wrote:
 
 My two cents is that it is not only the potential stress to the
sprinkler from removal/replacement, but the potential for damage during
handling.  This is especially true for QR sprinklers.
 
 From the EOR perspective, I have them replaced with new regardless of if
it could be kept in a drop.
 
 I understand there may be differing perspectives when you are in a
competitive bid that doesn't address the issue, or you have an owner griping
about every dollar spent.
 
 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 accentf...@aol.com
 Sent: Friday, February 06, 2015 4:05 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Relocate sprinklers with drops RETORT
 
 Good afternoon, All:
 
 I thought a previous discussion revealed that currently IF the sprinkler
stays in the RC, weld-o-let, fitting, etc., then it can be  reinstalled if
the sprinkler has not actually been removed from the original
fitting/outlet.
 I believe the concern was the amount of 'stress' applied to the
sprinkler when trying to remove it - and possible damage resulting from the
'torque'.
 Previously, everyone seemed to be on board with this  approach.
 
 Cordially-
 
 Jerry
 _accentfire@aol.com_ (mailto:accentf...@aol.com)
 
 *Jerry D. Watts, SFPE
 President  Co-Founder
 ACCENT FIRE ENGINEERING INT'L. Ltd.** Santa Fe, New Mexico USA
 (800) 503.1961 nationwide
 
 *New Mexico Journeyman Sprinklerfitter Lic.  #08228
 
 **Licensed Fire Protection Engineers -  Architects/Inspectors/Fire
 Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
 
 
 
 In a message dated 2/6/2015 2:04:42 P.M. Mountain Standard Time,
pe...@waynefire.com writes:
 
 Based on  the 2nd draft, this is what the 2016 language will say 
 unless it is  Successfully NITMAM ed
 
 6.2.1.1*
 When a sprinkler is removed  from a fitting or welded outlet, it shall
not be reinstalled except as  permitted by 6.2.1.1.1.
 6.2.1.1.1
 Dry sprinklers shall be  permitted

RE: day of questions - Hangars

2015-01-29 Thread Bill Brooks
I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the
building and the sprinkler system realize it isn't a NFPA 13 design and the
sprinklers operate differently (quicker and more effectively) with a slope
exceeding 2 in 12 then they do for a sprinkler system installed in a
different building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any
different unless the original specified design area included the increase
already?

Scott
 
Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a
statement NOT to increase design areas (though my experience has been that
we do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Bill Brooks
Yes, I'm also referencing the ETL.  Have you had your opinion confirmed by
MED FPE?  I've never considered the ceiling slope provisions to be a density
issue.  So maybe I've been an overly conservative designer.

Bill Brooks 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 4:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Bill - as Chris just pointed out, The Air Force ETL (which this thread is
discussing) references NFPA 13, but not for design densities. Because the
ETL defines the design densities, you cannot get to the sloped ceiling
requirements of NFPA 13 because they fall under the design densities section
of 13, which we are not referencing. Apparently - absent the specific
requirement by the ETL to increase design areas - the Air Force considers
sloped ceiling to be a non-issue in a high-ex foam / overhead sprinkler
system design (or that it is adequately addressed with the 5,000 sq.ft.
design area).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Bill Brooks
Sent: Thursday, January 29, 2015 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the
building and the sprinkler system realize it isn't a NFPA 13 design and the
sprinklers operate differently (quicker and more effectively) with a slope
exceeding 2 in 12 then they do for a sprinkler system installed in a
different building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any
different unless the original specified design area included the increase
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a
statement NOT to increase design areas (though my experience has been that
we do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Massive fire burning at Edgewater apartment complex | NJ.com

2015-01-23 Thread Bill Brooks
Exactly correct, public policy normally follows disastrous events.  In the
PA Fire and Panic Act days there was a huge fire which destroyed a shopping
mall.  Although it had a huge impact on the community in terms of jobs and
revenue, it was a successful code event in that no one died.  It will be
interesting to see if a 13 system would have mitigated the damage in this
case.  In hindsight the cost of a 13 system would seem to be pretty
economical for this property, but when you multiply the 13 cost by every
property in the state this still might be a cost effective code success.
Therefore no need to adjust your regulations.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Drucker
Sent: Friday, January 23, 2015 4:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Massive fire burning at Edgewater apartment complex | NJ.com

Pedestal 13R.  This is typical of the special provisions section. I did a
presentation at the NJ league of municipalities in 2013 on this type of
construction noting particularly where the measurements are taken (two
different places, ie height and stories). Fact is unprotected lightweight
wood frame (5B) and 13R are all about risk tolerance, ie what's acceptable.
If occupants getting out safely but losing the building is, then the
paradigm worked. Its really a matter of public policy. IBC special
provisions, NFPA 13R is just that. Hey I'm a firefighter/fire protection
guy, concrete 1A, NFPA 13, 14, 20, non combustible furnishings, smoke
detection, notification, etc etc works for me, then again I'm not writing
the check. We will see how public policy shapes our building and fire codes
going forward.

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823


Steve Leyton st...@protectiondesign.com wrote:

John:

Photos seem to show a 4-story type 5 with attic over a concrete podium.  Is
that the configuration?   Do we know if it was 13?  13R?  Looks like the
classic roof burn-off; I wonder if draftstops were compromised, or even
installed?   Lots and LOTS of questions  ...

SL


-Original Message-
From: Sprinklerforum on behalf of John Drucker
Sent: Wed 1/21/2015 7:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Massive fire burning at Edgewater apartment complex | NJ.com

http://www.nj.com/bergen/index.ssf/2015/01/crews_battling_fire_at_edgewater_
apartment_complex.html#incart_m-rpt-1

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Shadowed area behind built in cabinet and in widow sill

2014-10-06 Thread Bill Brooks
I see some worms peeking through the lid of the can.  Is this going to
spiral us down the EOR hole again or is this another hole occupied by
sprinkler designers/contractors?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rfletc...@aerofire.com
Sent: Monday, October 06, 2014 10:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

1.7 New Technology Nothing in this standard shall be intended to restrict
new technologies or alternate arrangements... Based on the recently
discussed conservative committee actions I would think that anything in the
later editions of 13 should be allowed as an alternate arrangement.  Say
something in 2002 edition that was later proved to be wrong through full
scale testing. Would you force a licensed contractor to install it wrong
because the AHJ hasn't adopted the standard with the new data with the
corrections? Or as a licensed contractor would you knowingly install
something that has been proven to be wrong by today's standards because it
was okay in the 2002 editionRon F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Monday, October 06, 2014 6:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

There are two lines of reasoning I have seen on matters such as this:
1.We aren't following the newer NFPA 13 - period.
2.The newer standard may have what the NFPA committee believes to be the
best criteria, but the ICC and our local codes folks have not weighed in on
the changes to the standard. Therefore, we cannot accept those
'clarifications.'

WE may KNOW that the changes won't affect the future code revisions; but the
AHJ doesn't know and most times won't take the chance.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of svang...@aerofire.com
Sent: Friday, October 03, 2014 7:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Shadowed area behind built in cabinet and in widow sill

We are bound to NFPA 13 (2002).  We have an ECHSW above the door in a room.
On the opposite wall is a window and sill that does not create an additional
floor area.  There is a built in cabinet that partially obstructs the window
sill and creates a shadow of 2 sq.ft. between the cabinet and the window
over the window sill.  We informed the AHJ that per NFPA 13 (2007) 8.5.3.2.4
sprinklers are spaced to walls and not windows if they do not create
additional floor area.  We also pointed to NFPA 13 (2013) 8.1.1(3) 
A.8.1.1(3) which indicate shadow areas are acceptable so long as the other
obstruction guidelines are followed.  The AHJ stated they cannot accept the
newer standard clarifications on this issue.

Is there something I am missing in NFPA 13 (2002) that states this design is
acceptable?

  Thanks,

Sean




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Cloud Ceiling Article in Sprinkler Age (Get Involved)

2014-09-19 Thread Bill Brooks
Brad, you need to 1) start submitting proposals and comments during the NFPA
Standards cycle, and/or 2) apply for a seat on one of the Technical
Committees.  It is an awakening process to see the way a typical committee
operates.  In my experience there is a handful of opinion leaders on each
committee who drive the process forward.  It's best to figure out who these
individuals are and attempt to understand their motivations.  The process is
set up to make it difficult to overturn committee actions.  This is good or
bad depending on your point of view.  All this said, it is actually possible
to affect a change if you are persistent.

The NFPA website has all the proposals and comments for each Standard, along
with the committee action.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: Friday, September 19, 2014 9:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Cloud Ceiling Article in Sprinkler Age

Good Article by Tom Wellen in current Sprinkler Age.

Tom did the original modeling in 2000, and came up with max gap width 8 (to
not need heads above).

The recent tests and modeling confirmed that, but showed it was reasonable
to extend it to allow 1 gap width per foot of ceiling height, so at 12'-0
ceiling height the gap between clouds could be 12 and not need heads above.

There are other rules that apply. 

I found it disturbing that the TC decided to go conservative after all
that and say 8 max gap width PERIOD. That really gives the Architects a lot
of leeway in the design phase... (frigging) NOT!

Design by Committee. That is something to NITMAM if I ever did see one, and
I will if I get a chance. 

 

Is there somewhere I can see whom voted for what on this issue, a link or
something? I've been stewing over this for a few days now, and it doesn't
help to 'talk it out'.

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

bcasterl...@fsc-inc.com

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: fume hood / dust collector - sprinklers in?

2014-09-08 Thread Bill Brooks
Another case of the difference between when required and how to do it.  The 
International Mechanical Code (2012) Sections 510 (Hazardous Exhaust Systems) 
and Section 511 (Dust, Stock and Refuse Conveying Systems) provide guidance on 
this.  Again, it shouldn't be up to a sprinkler contractor to figure out 
whether sprinklers should be installed but only to install per the appropriate 
standard.  As with most of these issues, we don't know if there is a design 
professional on this job or whether your regular customer has just installed a 
new process and has called you to do what's required.  At a minimum you should 
have a copy of the IMC which is enforced for this location.

So, someone (you??) must assess the installation per IMC Section 510/511  from 
end to end.  There is a suppression system reference in Section 510.7.  Some 
determination needs to be made as to whether the materials are nonflammable 
and noncombustible under all conditions and at any concentration then make the 
call on suppression.  The entire exhaust system must be engineered to meet the 
performance characteristics in the IMC.

Of course, local code amendments will govern as well as any local AHJ, 
insurance requirements etc.

Sprinkler contractors have a long history of being the can-do guys, with no 
good way to transfer scope responsibility to the right place.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Monday, September 08, 2014 7:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: fume hood / dust collector - sprinklers in?

I have a job where they have a small furnace to create molten metal for 
castings.  There is a hood (2x8ft) above the area where they take the used  
probes  and clean them off.  This duct work goes outside to a dust collector.  
How do I determine if sprinklers are needed in the hood and ductwork?

Thanks,

Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: fume hood / dust collector - sprinklers in?

2014-09-08 Thread Bill Brooks
Again, without any information about which codes are in effect, you should 
start with the IMC as I indicated earlier.  No one on this list can actually 
give you an answer, and, as Ron has shown, sprinklering everything is not 
always the correct answer.  Craig's response is pretty much what is necessary.  
In the absence of other information, perhaps you will have to hire someone to 
make the assessment.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Monday, September 08, 2014 12:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: fume hood / dust collector - sprinklers in?

There is no ME for the project and the HVAC contractor who is providing it 
brought up the question on whether sprinklers are required.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of craig.pr...@ch2m.com
Sent: Monday, September 08, 2014 11:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: fume hood / dust collector - sprinklers in?

Quite honestly you should throw this back to the owner/GC to have a mechanical 
engineer or vendor determine what is required per code.

There are several conditions to be considered.

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Dewayne Martinez
Sent: Monday, September 08, 2014 7:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: fume hood / dust collector - sprinklers in?

I have a job where they have a small furnace to create molten metal for 
castings.  There is a hood (2x8ft) above the area where they take the used  
probes  and clean them off.  This duct work goes outside to a dust collector.  
How do I determine if sprinklers are needed in the hood and ductwork?

Thanks,

Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Seismic bracing

2014-09-05 Thread Bill Brooks
Does anyone know if this is an actual standards requirement or just a
preference of the local AHJ ?

One way to do this would be to ask the AHJ.  This is something AHJ's are
supposed to know.  It is unusual for an AHJ to put himself/herself in the
middle between yourself and the building owner by dictating building code
requirements.  It is actually the Owner's responsibility (with advice from
the design professional's team) to figure this out.  However, you are being
given some good advice by others regarding the process involved.  The IBC,
along with ASCE 7, will provide the basis for the SDC C advice and there
could be a state or local code amendment which supplements the IBC.  Being
your project is in NC it's likely the IBC is used, but there could be other
jurisdictions where there is no adopted code or else it isn't the IBC or a
current edition of the IBC.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Sorrell
Sent: Friday, September 05, 2014 8:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Seismic bracing

I need some help with a seismic problem.
I am making modifications to a 1970's sprinkler system in NC, we are using
the 2000 ed of NFPA  13.
There is no seismic bracing on this system.
I have had to add some new main in various areas.
The local AHJ is requiring that only the new sprinkler main will need to be
braced.
Does anyone know if this is an actual standards requirement or just a
preference of the local AHJ ?
Obviously I am trying to avoid installing the seismic bracing on this
project.


Stephen J. Sorrell, CET
NICET# 77901 Level III
E mail: ssorr...@performancefire.commailto:ssorr...@performancefire.com

Performance Fire Protection, LLC
Corporate Office
179 Gasoline Alley -  PO Box 4510
Mooresville, NC 28117
Phone: 704-663-1664  Fax: 704-663-1652
Cell : 704-309-1242

Web: www.performancefire.comhttp://www.performancefire.com
Licensed in NC, SC, VA, TN, GA, AL

Performance on Every Level.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Simultaneous Fires

2014-05-15 Thread Bill Brooks
Has anyone had a design which considered the possibility of a fire in a
diesel pump house simultaneous with a fire in the protected property?
(Buildings are adequately separated).  The thought would be an upset
condition occurs with the pump while it is doing its job and a diesel fuel
fire is generated.

 

I've never been down this road before but there's always a something new out
there to discover.

 

Bill Brooks

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Can a hydrant flow from the pumper connection be used for the hydraulic calculations ?

2014-05-14 Thread Bill Brooks
Do these flow models know when a valve is closed?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Wednesday, May 14, 2014 11:48 AM
To: craig.pr...@ch2m.com; masorn...@kfi-eng.com;
sprinklerforum@lists.firesprinkler.org
Subject: RE: Can a hydrant flow from the pumper connection be used for the
hydraulic calculations ?

Now that I understand the intent of the topic ...

Ironically, this underscores something that's somewhat controversial and is
a current topic in the NFPA 14 revision cycle, i.e. currency of flow tests
and the use of flow models in lieu of open port flow testing.  If you're
dealing with a water agency that has their system(s) modeled, or uses a
third party to run flow models, it can be determined with a very high level
of accuracy just how much flow (and at what velocity) a particular leg or
main will produce.   Craig's point about a single 8 not likely producing
4,000 gpm may be true, but two or three 8 legs of a municipal grid
certainly can and that's where extrapolation of flow test results or the use
of a model can help a fire official determine whether a particular water
supply is capable of delivering the require fire flow to particular parcel.

BTW Mark Sornsin, I've already heard about this from others so if you want
to make fun of me anymore the line forms over there.

SL

 




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of craig.pr...@ch2m.com
Sent: Wednesday, May 14, 2014 7:41 AM
To: masorn...@kfi-eng.com; sprinklerforum@lists.firesprinkler.org
Subject: RE: Can a hydrant flow from the pumper connection be used for the
hydraulic calculations ?

I understand the purpose of the 20 psi value.  I have seen 20 psi values
that in no way would flow.  4000 gpm+ though an 8 water main, or a flow
value not achievable by the municipal water supply.  My point is there is a
danger in posting non-verified values in a flow report.  If you want to know
what's available at 20 psi then flow the system until it bottoms out at 20
psi then you have factual data.  Otherwise when it's needed most that
fictional 4000 gpm may only actually be half or less.  In the midst of a
fire fight, is not the time to find out reality and extrapolation are not
the same.  Now I realize that most project do not require large flow rates,
so it's typically not a big deal.  In the industrial world, it's a big deal.


We had a large project, water department did a flow test on a single hydrant
butt with less than 1000 gpm flowing, extrapolated the curve out and modeled
the water supply to the site which indicated we would have sufficient flow
and pressures for our system.  When the final pump test was performed the
flow rate was not there, not even close, the water department had assured
the owner of a robust water supply. In actuality, they had a lot of
water but their modeling was flawed and their test inconclusive due to
extrapolation and not actual verification.  The owner had to add an above
ground suction tank which delayed occupancy of the facility.   

Facts are facts and extrapolations are nothing but a good guess in many
cases.  

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Patterson Fire Pumps

2014-05-09 Thread Bill Brooks
Looking for a link to the Patterson fire pump selections - not just sales
brochures.  Looking for diesel drive, 2500 gpm options.

 

Thank you.

Bill Brooks

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Pump Electrical Service

2014-04-05 Thread Bill Brooks
Are you saying the utility is not supplying the correct voltage and a
transformer is needed between the pump controller and the primary service
disconnect?

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Don
Lowry
Sent: Saturday, April 05, 2014 1:11 PM
To: sprinklerfo...@firesprinkler.org
Subject: Fire Pump Electrical Service

References from NFPA-20 (2010 edition) 

Situation:

Fire Pump to be installed on ESFR system  (75 hp) electric motor.
9.2.2 (1) or (5)

On down through Chapter 9  to;

9.2.3.4 Where the overcurrent protection permitted by 9.2.3 is installed,
the overcurrent protection device shall be rated to carry indefinitely the
sum of the locked rotor current of the fire pump motor(s) and the pressure
maintenance pump motor(
s) and the full-load current of the associated fire pump accessory
equipment.

OK, so the locked rotor current is 543 amps, plus jockey pump, lights, heat,
etc added would require a 600 amp over current protective device.  This is
what the Engineer and I determined would be the requirement for this
dedicated service to the fire pump.

When the engineer submitted his electrical service plan (600 amp service) to
the city, the City Plan Reviewer states that we don't need a 600 amp
service, but rather a 125 amp service.

In reading through Article 695.4 of the NEC. It states:
 Where the locked rotor current value does not correspond to a standard
overcurrent device size, the next standard overcurrent device size shall be
used in accordance with 240.6.  The requirement to carry the locked rotor
currents indefinitely shall not apply to conductors or devices other than
overcurrent devices in the fire pump motor circuits. 

So, does this mean that the service itself (transformer) and related
conductors can be per normal size (125 amp) with just a 600 amp fuse in the
disconnect before the controller?

In 30 + years this is the first time I have ever been asked about this.
Before I was only asked about pump size etc , and when installed and checked
at pump start-up there was indeed a fuse of appropriate size in the service
disconnect.  So I assumed all was correct.  I'm just wanting to make sure
the Engineer and I understand the requirements for the actual electrical
service provided.  I know it's not my area of expertise, nor my
responsibility, just curious.

Thanks in advance for any help.

Don Lowry, CET, RME (TX)











___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 1978 NFPA 13 question

2014-03-24 Thread Bill Brooks
This would have been based on NFPA 231, 1974 edition.  Class III storage, 25
ft high.  Basic density of 0.19 over 4000 but a 140% density multiplier for
25 ft storage.  In those days Class III was wood, paper, natural fiber cloth
or products thereof with or without pallets.  Products contain a limited
amount of plastics.  Metal bicycles with plastic handles, pedals, seats and
tires is an example of a commodity with a limited amount of plastic.  500
hose, not sure about the 600 number. 

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, March 24, 2014 2:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: 1978 NFPA 13 question

I'm looking for the definition of what was covered by an Ordinary Hazard
Group 3 classification based on the 1978 NFPA 13.

I have a warehouse designed at .26/4000 with 600 gpm hose stream allowance,
Ordinary Hazard Group 3.  It was a preaction system with area heat
detection.  (non-heated whse).  

Trying to figure out what the EOR was basing the design on as far as
anticipated type of storage.

25 ft high piled (no racks), 35 ft high ceiling.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Bill Brooks
This is not the why group.  This is the follow-the-rules group, which
includes engineers, educators, AHJs, designers, installers, and
manufacturers, because NFPA 13 is a rule book and not an engineering guide.
If you want to reach the why group, submit Proposals to the NFPA 13
committee during the Proposal period, or begin sending Comments during the
Comment period.  By doing this you will get direct feedback in the form of
Committee Responses directly addressing your concerns.  Send them your good
ideas, then challenge them all the way to the Standards Council if you wish.
You sound like the kind of person who would enjoy the jousting.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Thursday, March 13, 2014 2:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

True enough! Actually, there are quite a few ceiling height changes and
surface mounted lights and other fixtures.
Thank you very much Vince. You are one of the few whom did not reply to my
Why? why? why? with DONT WORRY ABOUT IT JUST DO IT

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, March 13, 2014 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad

 *i hope you are not ashamed of that-- I am not your fault! :) !

 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 I think it'll work fine. Why deep plates?

 Vince


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pump House Controls

2014-03-07 Thread Bill Brooks
What do you have to say about a triple pump arrangement with 7500 gpm total
capacity being fed by a 10 supply?  Wouldn't this mean the system was
designed for 2500 gpm demand?  Maybe I'm missing some other information
about the existing set-up.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tom
Duross
Sent: Thursday, March 06, 2014 7:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Pump House Controls

I have a question regarding how you guys would control this.

Outside pump house with aboveground tank, 500,000 gal.
Three diesel drive fire pumps in parallel from 10 tank supply to 10 yard
supply.
All three pumps are rated at 2500 GPM but different pressure ratings.
I have no design information right now but it's a record storage facility,
50' high piles of paper, fwiw.
I'm looking at replacing one of the pumps, the oldest and original, I'll
call it pump #1.
Pump #1, original 1971 is a 10x8 rated for 2500@125 PSI.
Pump #2 was replaced in 2003, same model 10x8, nice tier 2, 2500@125.
Check.
Pump #3 was replaced in 1994, same model 10x8, but 2000@65.  Huh?
Jockeys are dual vertical turbine, 100@140.  Check.
If I work under the premise of direct replacement and quote a 2500@125, tier
3 or 4,
how would you guys balance these pumps for lead to lag with a pump so small
compared to the rest?
Pump #2 becomes the lead pump and #1 and #3 fall in 10# each behind?
TD


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: seismic bracing calcs

2014-02-21 Thread Bill Brooks
Exactly.  Unless your drawing which shows those little criss-cross arrows
are accompanied by calculations AND unless your calculations are acceptable
to the project structural engineer, then you do not have a complete package
that's ready for installation.

As we've seen for many years on this forum, sprinkler contractors have been
assuming the responsibility of architects and various types of engineers,
and even the owners themselves by worrying about what they intend to put in
their swimming pools when they drain it (just as an example!).  Mostly out
of necessity and really bad performance design documents.  I sympathize
with all of you who want to do things right but are faced with a tangle of
ineptitude by so many others.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Friday, February 21, 2014 12:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs

How do you locate per 13? How do you know what you did will work? How do you
know that 1 x 34 brace at 37 degrees to side of a beam doesn't need to be
shorter, at a different angle, or a 1 1/4 brace, without doing calcs? 13
only tells you the general and minimal places where the braces need to go,
lateral and longitudinal, but you ned to do the work and then prove it. Why
then would you not include the calcs in your submittal?


On Thu, Feb 20, 2014 at 8:57 PM, Forest Wilson Fire Sprinkler Contractor 
forest_wil...@aol.com wrote:

 Locate per 13 and send a calc sheet only if required in plan review.



 Forest Wilson
 Fire Sprinkler Contractor
 937-736-0425

 Notice:
 This message is confidential. It may also be privileged or otherwise 
 protected by work product immunity or other legal rules. If you have 
 received it by mistake, please let us know by e-mail reply and delete 
 it from your system; you may not copy this message or disclose its 
 contents to anyone. Please send us by fax any message containing 
 deadlines as incoming e-mails are not screened for response deadlines. 
 The integrity and security of this message cannot be guaranteed on the
Internet.

  Original message 
 From: rongreenman . rongreen...@gmail.com
 Date:02/20/2014  11:36 AM  (GMT-05:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: seismic bracing calcs

 From the Piemontesi to the greasy Sicilian, with molte amore. I won't 
 hold it against you that your family is from the rock of hell in the 
 Med 'cause you always explain the problem so clearly. And Letyon's OK too.


 On Thu, Feb 20, 2014 at 8:09 AM, Steve Leyton 
 st...@protectiondesign.com
 wrote:

  Right - all of the above.   We put the calc's on our detail sheet(s)
  next to enlarged sketches of the proposed anchorage.
 
  Steve L.
 
 
 
 
  -Original Message-
  From: sprinklerforum-boun...@lists.firesprinkler.org
  [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
  Brian Harris
  Sent: Thursday, February 20, 2014 6:32 AM
  To: sprinklerforum@lists.firesprinkler.org
  Subject: RE: seismic bracing calcs
 
  Both...
 
  Brian Harris, CET
  BVS Systems Inc.
  bvssytemsinc.com
 
  -Original Message-
  From: sprinklerforum-boun...@lists.firesprinkler.org
  [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
  craig.pr...@ch2m.com
  Sent: Thursday, February 20, 2014 9:27 AM
  To: sprinklerforum@lists.firesprinkler.org
  Subject: seismic bracing calcs
 
  Seismic design category C, contractor submittal package,
 
  Do you provide a calc sheet for EQ bracing or just locate per NFPA 
  13 and send typical catalog data sheets?
 
  FM Global project, BTW.
 
  Craig L. Prahl, CET
  Fire Protection Group Lead
  CH2MHILL
  Lockwood Greene
  1500 International Drive
  Spartanburg, SC  29303
  Direct - 864.599.4102
  Fax - 864.599.8439
  CH2MHILL Extension  74102
  craig.pr...@ch2m.com
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
  kler
  .org
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
  kler
  .org
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 



 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405

 rgreen...@bates.ctc.edu

 http://www.bates.ctc.edu/fireprotection/

 253.680.7346
 253.576.9700 (cell)

 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

 They are happy men whose natures sort with their vocations. -Francis 
 Bacon

RE: seismic bracing calcs

2014-02-20 Thread Bill Brooks
I have specified the shop drawings and bracing calculations be submitted to
the project structural engineer to confirm the adequacy of the attachment
point to resist the loading.  Is this a common practice?

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, February 20, 2014 4:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs

And we haven't gotten approval for a document set without including all of
those things in, like, forever.Standards of care and regional best
practices ...


Steve Leyton




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, February 20, 2014 11:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs

Steven,

I have never received a contractor shop drawing that covered things to the
detail you describe.  It's often a wonder to get the basic information on
the drawings like pipe elevations and hangers let alone anything to the
depth you describe.

I don't disagree with your statement just saying, I've never seen it happen.


Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven
Scandaliato
Sent: Thursday, February 20, 2014 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: seismic bracing calcs

Wait...hold on...just to make sure, and Craig I am sure you probably know
this...BUT we have a lot more than just calcs for braces that have to be
addressed.  We have 4 other design features that have to be addressed.
Cplgs, clearance, separation and restraint.  This is a weakest link kinda
thing...so just because we have braced a system does not mean it is designed
for seismic...we have to put flex and rigid cplgs where they go, we have to
show that we have accounted for clearance where it applies, we have to
acknowledge that there is no separation required if applicable and we have
to show and space b'line restraint.  Seismic design demands its own sheets
and symbols and sheet installation notes etc.  Do not try and pile all of
this onto an already unreadable piping plan.  EOR or Shop design, all of
these categories must be addressed in the documentsand by the way,
putting 4-ways and every change of direction is not a design feature
required or intended by 9.3.  I see a lot of contractors do that thinking
they are in compliance.  This may be a great cost saver or standardized
thing you want to do with your fitters but it does not automatically put you
in compliance with 9.3just sayin.

One other note while I am on this, we all need to pay better attention to
restraint.  I still have many AHJs and contractors alike that haven't heard
of it.  If seismic is required then restraint is required.  This isn't
optional.  And pay attention to the spacing requirements for it.  Many,
including myself, have fallen into the end of line mentality and think
that is the only place we have to have it...but if you have long
branchlines, you definitely will have more than end of line locations.

With Sicilian Love,

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Thursday, February 20, 2014 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: seismic bracing calcs

Cliff's opinion is right.


On Thu, Feb 20, 2014 at 6:49 AM, Cliff Whitfield
cl...@fire-design.comwrote:

 Craig,

 If you don't calc it, how do you know it works?  That would be like 
 sending in drawings with 'hydraulically calculated pipe sizes' with no 
 hydraulic calcs to prove the sizes are correct.  Just not happening.

 A lot of 'East Coast' contractors/designers (I fit in that category 
 even though I now live in Colorado) just show braces on their drawings 
 but it's not even close to being the correct way to do it.  They need 
 to take the time to learn from the AFSA classes that Ken Wagonner and 
 others do so that they can do it right.  I've had to take it 3 times 
 because I don't use it very often and it easy to forget without the 
 repetition but it's just something you have to do if you are doing 
 your
job correctly.

 Simply my opinion (but I think it's right!)

 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479



 cl...@fire-design.com
 www.fire-design.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org

NFPA 13 Future Development

2014-01-30 Thread Bill Brooks
Perhaps a question for Roland or other committee members.

What is the big picture with regard to the coordination of FM 2-0, 8-9, etc.
with NFPA 13?  Are we going to see two competing sprinkler standards in a
few years?  Will the sprinkler requirements in NFPA 30 be merged with NFPA
13 at some point?

Bill Brooks

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Transfer Switch Tests

2013-10-30 Thread Bill Brooks
Not covered on the AFSA webinar either.

One of my recurring concerns for the NFPA system is the ratio of People Who
Get Paid for Stuff / People Who Actually Pay for Stuff.  NFPA 25 is about 10
to 1 but can you consider large organization reps in the category of payers?
That would be GSA rep, VA rep, DOE rep, and Home Depot rep.

The Home Depot rep made the presentation so I'd assume there is more (or
less) to this than meets the eye.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John
Denhardt
Sent: Tuesday, October 29, 2013 11:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Transfer Switch Tests

From the 25 - 2014 ROP

25-187 Log #249 Final Action: Accept in Principle
(8.3.3.4(3) (New) )
___
Submitter: John Whitney, Clarke Fire Protection Products, Inc.
Recommendation: Revise text to add; Verify that pump continues to perform at
peak load on the alternate power source for 10 minutes or 30 minutes if
alternate power source is a standby generator set.
Substantiation: During annual tests it is only appropriate that the
alternate power source also be tested to assure that circuits and generators
be tested to confirm they perform under peak load. 
Committee Meeting Action: Accept in Principle Add peak horsepower before
load. 
Verify that pump continues to perform at peak horsepower load on the
alternate power source for 10 minutes for a alternate utility or 30 minutes
if the alternate power source is a standby generator set. 
Committee Statement: Clarifies that a standby generator requires a 30 minute
test while carrying peak electric motor fire pump horsepower load. 
Number Eligible to Vote: 33
Ballot Results: Affirmative: 33 


WOW! - No negative votes!  No comments!


John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A.
Sornsin, P.E.
Sent: Tuesday, October 29, 2013 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Transfer Switch Tests

All of a sudden, flow meters piped back to suction (or suction tank) look
like a good thing - at least when you need to test transfer switches.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tom
Duross
Sent: Monday, October 28, 2013 6:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Transfer Switch Tests

Can't be every year, really?
I think (or hope) that's a misprint because flowing 150% for 30 minutes is
beyond ridiculous.
No, there is no other way to put peak load on the driver other than to pump.

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John
Denhardt
Sent: Monday, October 28, 2013 6:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Transfer Switch Tests

Agree every year.  But what about the 30 minutes flowing water.  Is there
another way to simulate peak load?

Sent from my Motorola Smartphone on the Now Network from Sprint!


-Original message-
From: Tom ihaveakub...@yahoo.com
To: sprinklerforum@lists.firesprinkler.org
sprinklerforum@lists.firesprinkler.org
Sent: Mon, Oct 28, 2013 18:36:03 EDT
Subject: Re: Transfer Switch Tests

Tom,

Not sure if  you are referring to annual testing (NFPA 25) or acceptance
testing (NFPA 20) ? If NFPA 25 I believe the transfer test is required
annually not every 3 years.

Tom
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com

RE: Hazard classification

2013-07-26 Thread Bill Brooks
Take it from me - it is a small sum, generally some percentage of the
overall construction cost as doled out by the architect. For some reason we
can do performance sprinkler design but the plumbers still draw piping
diagrams showing the cold on the right and the hot on the left.  Why that
can't be performance I'm not sure.

(It's Friday)

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A.
Sornsin, P.E.
Sent: Friday, July 26, 2013 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Hazard classification

I've shared this before I think, but it seems apt again:

I once pursued an A/E project where I felt the owner was seeking actual
engineering from the engineer of record for the fire sprinkler system. I
suggested to our team that we propose doing just that and sell ourselves as
providing a complete design for the sprinkler contractors to bid
apples-to-apples.  The mechanical engineer on the team (from a different
company) suggested that taking on the design of the sprinkler system might
be taking on too much risk/liability (after all, MEs are used to performance
specs - usually without the performance part - my words not his).

That solidified my understanding of the MEs' approach to fire sprinkler
systems. Not sure how they justify receiving payment for what they provide
(unless it's a really small sum).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Craig
Leadbetter
Sent: Thursday, July 25, 2013 5:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Hazard classification

Dwight,

I love the optimism that there is actually a spec to look at that says more
than provide a system per code. No mention of commodities types on the plans
and if I asked I have sure I would get the deer in the head lights look.

This has been great discussion on this topic, it confirms that my area of
the country is not the only one that provides more questions than answers. I
believe that most systems we see are under analyzed from a fire suppression
stand point. Most engineers appear to be so afraid to put anything in
writing when it comes to fire protection that we generally get an X
through the drawings with a note to provide per all codes and insurance
requirements, and add any additional heads at no cost to the owner.

Craig Leadbetter

_
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: BK Design

2013-07-26 Thread Bill Brooks
Wouldn't 634 sq ft be partial?

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill,
Christopher
Sent: Friday, July 26, 2013 12:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: BK Design

Trying to figure out if you are disagreeing with Curtis other than the
reference to latest code.  You are right you follow the code in effect as to
whether you need sprinklers.  So there are differences in which edition in
whether they are required.  But if not required and you choose to go over
and above you are still obligated to follow the referenced standard (and
year) of the adopted code.  See IFC 2006 (and '03 and I still think it's in
'12) 901.4.2 Nonrequired fire protection systems. Any fire protection system
or portion thereof not required by this code or the International Building
Code shall be allowed to be furnished for partial or complete protection
provided such installed system meets the requirements of this code and the
International Building Code.

So you can't do a 634 sq ft system. Now there is a question about doing
above the ceiling with the phrase for partial...but generally AHJ's rule
either all of 13 or no sprinkler (when allowed to be non-sprinklered).
Could one say they are doing a full 13 design below the ceiling or I suppose
the same question is if you only do 634 sq ft in the building then you have
a 634 sq ft design (notwithstanding the phantom design area if in the '13
13).

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns 
McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron
Greenman
Sent: Friday, July 26, 2013 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: BK Design

Curtis,

You're obligated to design to the current adopted code of the jurisdiction
which may or may not be the latest codes and standards. And if this
building is a stand alone of 5000 sqft, with an occupancy of 100 it
doesn't need to be sprinklered at all per IBC (see requirements for an A-2
occupancy). If the applicable building code is IBC 2003 (I think it changed
in 2006 but maybe 2009--the prior threshold being 12K sqft and 300
people), or some earlier version, or one of the other model codes from the
Twentieth Century, or any code amended upon adoption by a state legislature,
or an amended municipal or county code (acceptable in home rule states), or
the code adopted in a major city, requirements can be wholly different
either requiring more or less protection. If BK has chosen to provide what
is essentially a volunteer life safety type system to provide customers
added egress protection in case of emergency (pretty standard thinking in A
and R type occupancies in the late seventies, through the eighties and into
the early nineties) in an otherwise non-required building I applaud them.
That it hasn't been revisited by the corporation since 1978 is troubling but
it's their decision. Personally I feel I'm pretty savvy as to how a fire
works and what threat I'm exposed to in the dining area of a stand alone
corporate fast food joint, and don't even give it a second thought as to
where I sit other than noting where the exits are.

Now if it's in a strip mall or a high rise or a full mall it's going to be
fully sprinklered because of the type of building it's in, first and
foremost because these buildings will already be sprinklered (at least
relatively new ones), and secondly because it poses a greater exposure
threat to it's neighbors, not necessarily its customers.

More prevalent on the fire alarm forum than here is an attitude of' If a
little is good, then the most is best. This is eventually self defeating as
other interests have larger stakes in buildings than fire guys and fire
protection contractors , and the concept of cost/benefit and diminishing
returns has to be considered from the customers' point of view. The
engineers are supposed to be doing this, but while the design/build model is
prevalent it's incumbent upon the contractors and techs to study up on this
stuff and incorporate it into their thought processes. I'm not directing
these comments at you Curtis, even though it was your comment that put me on
this track, but rather just in general. Nothing makes my head explode more
than a spec calling for a double-interlock pre-action system covering a
closet with a single rack of five or six PC type servers. Not only an
unnecessary expense in this case but the wrong system, spec'd because
someone thought if single-action is good double-action must be better. Damn
it Jim, I'm no accountant but even I know it's cheaper

RE: BK Design

2013-07-25 Thread Bill Brooks
Perhaps a non-required system if bldg fire area  5000 or  100 person
occupant loading (2012 IBC 903.2.1.2).  Then 901.2 Exception would say a
system is permitted to be installed for partial or complete protection
provided that such system meets the requirements of this code.

I'd say a letter to the contractor would be the next step, referring to the
code sections above.  Meets the requirements could be broadly interpreted
to mean sprinklering only a part of the building, selecting materials per
NFPA 13, spacing heads per NFPA 13, or some other selection of requirements
from NFPA 13.

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bob
Sent: Thursday, July 25, 2013 1:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: BK Design

I'm working on a Burger King.  I've never done a BK before, so what I'm
about to describe seems ridiculous.
The design criteria is based on a PE proto type from 1978.  This is what the
contractor was given and told to use as spec.
There are combustible concealed spaces above ceilings throughout premises,
but no sprinkler protection is to be provided.  The design criteria is 6
sprinklers over 653 sf in the dining area.  To be calc'ed light hazard.
That's it.  Has anyone out here in forum land provided the system for a BK
lately?  What was required/done?

Thanks,

Bob Knight, CET III
208-318-3057
www.firebyknight.com




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: George L. Church, Jr.

2013-06-27 Thread Bill Brooks
Some guy from Anchor Fire Protection introduced me to the list back in 1998.
My response was something like maybe you should switch to decaf. Not
knowing George well at the time I had no idea about his passion for things
which extended way beyond his job - like his continuing support for this
list and the AFSA. There's nobody out there who could get things done like
George.  Impossible situations could be reduced to solutions in a single
phone call and the next day implemented in the field. I had the privilege to
work for George as a reviewer on a number of projects years ago.  What I
found to be surprising was his ability to say OK we'll take care of it no
matter what the deadline or consequence.  I also know he valued his wife as
a true partner inside and outside the office - something all of us attempt
but are not always successful in achieving.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ken
Holsopple
Sent: Thursday, June 27, 2013 10:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: George L. Church, Jr.

Dear Forumites,

It is with great sorrow that I bear the news that George L. Church, Jr. past
away last evening after a 16 month battle with lung cancer.
George was 58 years old. George leaves behind a wife Cathy, daughter
Margaret (Meg) Ames, son-in law Dave Ames, his mother and four sisters.

George's sprinkler career started in 1974 with Automatic Sprinkler
Corporation of America (Philly) and in 1998 started Rowe Sprinkler with his
wife Cathy.
As many of you know, he was a fan of this forum and an huge advocate for the
fire sprinkler industry. He served on several NFPA committees and valued the
many friends he made along his journey.
His humor, enthusiasm, and passion for the sprinkler business will be a
great loss for all of us.

I will post funeral arrangements here on the forum when they become
available.

But in true George Church fashion and as a tribute and continuation of his
last forum postI know he is licking (kicking) himself in a better place.
(Sorry Mr. Muncy, but I know he wouldn't have passed this one up.)

Wiping away tears as I hit the send button.

Ken Holsopple
Rowe Sprinkler Systems, Inc.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Contact

2013-06-16 Thread Bill Brooks
Scot,

I've taken the liberty to pass your email address on to a young fire
protection engineer who works for the Corps of Engineers. I just spent a
month with him in Afghanistan and he is in need of some advice with respect
to the relationship between US and European standards. I told him you are
the best I hope I'm not exaggerating!!

Thanks.  His name is Drew Lange (pronounced Lang ie two syllables).

Bill Brooks


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: fire pump controller detection requirement

2013-05-07 Thread Bill Brooks
So, if it does not have a secondary power source it would not be a Dedicated
Function Fire Alarm Control Unit?

I don't believe the committee had a fire pump controller in mind when this
change was made. I never have thought of a fire pump controller as a
component of a fire alarm system, but I'm willing to be educated.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Failla,
Daniel
Sent: Tuesday, May 07, 2013 2:52 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: fire pump controller detection requirement

Tim,

First I am working under the IFC 2012 that requires sprinkler systems to be
electronically monitored with supervising central station.

Per Section NFPA 72, 2010 10.15  and the definitions of a Fire Alarm Control
Unit and Dedicated Function Fire Alarm Control Unit, a smoke detector is
required to be located above the fire pump control panel.

Daniel S. Failla Jr.
Assistant Fire Marshal
Charleston Fire Marshal's Office
75 Calhoun Street
3rd Floor
Charleston, SC 29401
Office - 843 - 724 - 5960
Email: fail...@charleston-sc.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Easter,
Timothy
Sent: Tuesday, May 07, 2013 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: fire pump controller detection requirement

I know smoke detectors are required within 5' of FACP/MNS panels, what about
fire pump controller panels?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Looking for ideas- Fire Protection Engineering presentations

2013-02-05 Thread Bill Brooks
I like the idea of linking significant fire events to corresponding advances
in fire protection and code development.  Use of examples such as photos of
fires that destroyed major portions of US cities (San Francisco, Chicago,
Baltimore - most cities have had a significant fire) and link these photos
to early efforts to develop building codes. Explain the evolution of codes
from the aspect of preventing the destruction of neighboring property
(substantial construction materials) to where we are today in theoretically
preventing multiple life loss (sprinkler system installation).  Note the
corresponding fire testing that has followed major fire events like fire
resistance testing that began with studies of fuel loading in buildings and
the development of the time/temperature curve. Maybe cite the GM fire at
Livonia Michigan where the roof burned off an entire building.  Then there
is the Our Lady of Angels fire in Chicago that resulted in the E84 test
which of course was used to classify foam plastics until we found that foam
burned differently when it was installed vertically which resulted in yet
another test method.  I'd note the Cape Canaveral pad fire when three
astronauts were killed and the resulting changes based on high oxygen
concentrations.  Then the 9/11 towers collapse where CFD modeling and other
methods are used to explain some of the events of that day.  You could look
at the various testing agencies that develop new technology or products
using actual fire testing.  Maybe a rack test from UL or FM would be a good
video clip.

I'd also note the efforts of the three persons in the U.S. who have made
fire protection engineering a profession. John Bryan, founder of the MD FPE
program, who stayed with this program and its eventual accreditation even
though he could have moved in other directions throughout his career. Bud
Nelson, instigator of engineering methods, who saw the possibilities of
transferring mathematical methods to prediction of fire effects and the
development of performance design through the goal oriented systems
approach. Rolf Jensen, who was part of the Illinois Institute of Technology
program till he found the rewards of consulting following the McCormick
Place fire in Chicago. 

For something to take home with the students, perhaps assign them the task
of determining if their homes have smoke detectors, if their family has a
pre-fire plan, if their smoke detectors are photoelectric or ionization, and
whether they have CO detection in case of fireplaces, fuel gas appliances,
or attached garages.

All of this is engineering in one form or another and the idea is not to
focus just on a sprinkler going off and fixing all our problems (even this
would go a long way toward that end).

Excuse my MD bias, I can't help myself.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, February 05, 2013 9:34 AM
To: sprinklerforum@firesprinkler.org
Subject: Looking for ideas- Fire Protection Engineering presentations

We have Engineers Week coming up in a couple of weeks and our industry has
never had any representation for Fire Protection.

I was wondering if anyone has done one of these type of presentations and
had anything to use as a go-by?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Replacing heads after a fire

2013-01-17 Thread Bill Brooks
But here's a follow-up question - who is the appropriate individual to make
this determination? In my opinion this is not the sprinkler contractor.
Please read the word not as if I had capitalized it.

Just my opinion.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill,
Christopher
Sent: Thursday, January 17, 2013 1:11 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Replacing heads after a fire

2 is all required in your example, well if you want to return to service. 

The heat cooling cycle of the glass bulbs are repeated cycles to very near
operating temperature as I understand it.  One more cycle if it takes 100's
or more cycles won't make a difference.  The first 99 are the problem. 

On the creep of solder its sustained temperatures near operation as I
understand it.  This is a problem not a single fire. 

On the acid - well smoke comes in all flavors.  I'm certainly no chemist but
with that logic why are we not replacing the structural components or the
plumbing etc.?  Weren't they also damaged by the acid smoke?  I think where
acid is an issue is in sensitive electronics.  Think of the difference in
surface area.   And I don't understand the burn/smoke radius part.  The burn
radius of a sprinkler controlled fire is on the order of 1 to ten's of feet.
The smoke is often the entire building.  Not sure you need to go next door
and replace sprinkler head to get 2 rings past, lol.  

What I typically see is out of an abundance of caution replace the fused
heads and the first ring around.  But I don't think it has any technical
merit. Once the fitter is there a couple more heads is cheap to make
everyone feel good.  In the end I wouldn't balk if you replace the 2 and if
someone pays you for more, good for you.  

Good discussion item.  Often we don't get truly new things to banter about
on this forum. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns 
McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ben Young
Sent: Thursday, January 17, 2013 11:41 AM
To: sprinklerforum@firesprinkler.org
Subject: Replacing heads after a fire

This was a hypothetical question asked by one of our inspectors the other
day, and I did not know the answer.  Thought I would see if anyone else here
might know where this is written in black and white.

Say you have a large room with 20+ heads, or an open warehouse area.  The
building is fully sprinkled, and everything else is normal / SOP.

They have a fire in this room/area, and lets say, two heads activate and
control the fire.

The question is, how many of the heads do you have to replace?  Is there a
code requirements for this that exists?  I found some anecdotal evidence
from someone in the industry with more experience than I, but the only thing
close I could find in the codes was the NFPA 25 stuff relating to loading on
sprinkler heads.

I looked at NFPA's list of codes online, and saw some that may have some
information on this (NFPA 902 and 904) but they were withdrawn in 2001, and
I cannot view them online.

Obviously from a liability standpoint, you would want to replace as many of
the heads as possible, if not all of them, but what if you had a 500K SQFT
warehouse that was all open, would you want to replace all of them?

Here's the information that I got from my friend who's been around a while.
-If they're link heads, you want to probably replace all the heads, since
the acids in the smoke will impact the solder -Look at the burn/smoke radius
from the fire, and replace the heads around this area for the next two rings
of sprinkler heads.

He couldn't tell me where this came from, it was just the way it was always
done.

Is there a hard and fast rule for this?  Is it an insurance carrier or head
manufacturer judgement call?  Would rapid heating and cooling cause glass
bulbs to weaken or micro-fracture down the road?


Thanks,


Benjamin Young
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130117/93248633/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo

RE: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread Bill Brooks
In my case the rack uprights were 10' 4 but with only two pallet loads. It
caused the addition of an extra sprinkler even after much writing and
attempted explaining of the rack uprights being the transverse flue.  I
don't think this was the intent but it sure is written this way. It's an
unusual looking in-rack arrangement.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... 
Sent: Tuesday, January 15, 2013 1:38 PM
To: SprinklerFORUM@firesprinkler.org
Subject: Maximum in-rack sprinkler spacing - plastic over 25ft

Wayne:

You make a good point.

Per NFPA 13 in-rack sprinkler layouts,  I don't perceive that a gap between
pallets constitutes a formal transverse flue.   I think the transverse flue
is
formed by the steel column of the racking structure.

Wayne, you are correct in that 2007 NPFA 13 Figure 17.3.1.2(a) includes the
exception-to-the-rule of having in-rack sprinklers in each transverse flue
(TF) for plastic storage in open racks two-or-more-bays deep, [1] that
stores commodities at heights 25+ ft..  NFPA 13 however, mitigates the
reduction of in-rack sprinklers (particularly, but not exclusively) at every
transverse flue.  For the case of Figure 17.3.1.2(a), this mitigation calls
for horizontal barriers above each level of in-rack sprinkler *with
face-sprinklers*.  Does our situation you are describing contain such
horizontal barriers in the racking scheme?

One *could* assume (at least I do) that the horizontal spacing between in
rack sprinklers in Figure 17.3.1.2(a) is not to exceed 10 ft, as this is
maximum width of two pallets mentioned in Note 7 of this Figure.  This
maximum horizontal spacing between in-rack sprinklers is enforced even if
metal racking support columns are spaced greater than 10 ft apart.


[1]  new criteria added to this comment.

scot deal
Excelsior Fire



On Tue, Jan 15, 2013 at 4:03 PM, Dewayn
e Martinez deway...@dbfp.net wrote:

 Thanks Scot,
 What is confusing is that you are allowed to have more loads in the 
 vertical as long as you don't go past 10ft spacing but nothing is 
 mentioned for the horizontal spacing.

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20130115/33812f1b/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Underwater Tank Inspection

2013-01-08 Thread Bill Brooks
Anyone out there been involved in a project where you conducted an
underwater inspection of a tank? Did you use a diver or remote camera? I'm
trying to specify such an inspection and I'm looking for some suggestions.

Thanks.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Underwater Tank Inspection

2013-01-08 Thread Bill Brooks
The tank is 40 ft diameter, 300,000 gallons. Just trying to develop a list
of steps and associated equipment and personnel needed to produce an NFPA 25
report that would be acceptable to about 99% of the AHJ population.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Tuesday, January 08, 2013 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Underwater Tank Inspection

Bill,

I am curious about the application. Can you share more details about this
underwater tank?

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, January 08, 2013 8:00 AM
To: sprinklerforum@firesprinkler.org
Subject: Underwater Tank Inspection

Anyone out there been involved in a project where you conducted an
underwater inspection of a tank? Did you use a diver or remote camera? I'm
trying to specify such an inspection and I'm looking for some suggestions.

Thanks.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


NFPA 20 Shop Drawings

2012-12-20 Thread Bill Brooks
Seems as though there are no documentation requirements in NFPA 20 (like
NFPA 13, Chapter 22) when it comes to submittals and acceptance test
results.  Am I missing the obvious? 

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: NFPA 20 Shop Drawings

2012-12-20 Thread Bill Brooks
My interest is general at this point. However, I am preparing a
specification for a job which will require the preparation of fire pump
installation documentation. I thought I'd go right to NFPA 20 to find what's
needed, but it's not there as has been pointed out.

Seems each NFPA Standard should have a chapter which describes the minimum
amount of information needed to adequately document compliance. 

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bruce Verhei
Sent: Thursday, December 20, 2012 4:52 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: NFPA 20 Shop Drawings

What does the ahj have on their website?

bv

-Original message-
From: Steve Leyton st...@protectiondesign.com
To: sprinklerforum@firesprinkler.org
Sent: Thu, Dec 20, 2012 21:31:14 GMT+00:00
Subject: RE: NFPA 20 Shop Drawings

You're right about there not being an explicit prescriptive for pump system
plans.  But if I were an AHJ, I'd throw the applicable subsections of NFPA
13, Chapter 23 at the issue, such as 23.1.3(11),
23.2.1.   As for detailing the pump room, that falls squarely into of
23.1.3 and the provisions for hydraulic calc's and substantiating
calc's.   


Steve Leyton




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, December 20, 2012 1:24 PM
To: sprinklerforum@firesprinkler.org
Subject: NFPA 20 Shop Drawings

Seems as though there are no documentation requirements in NFPA 20 (like
NFPA 13, Chapter 22) when it comes to submittals and acceptance test
results.  Am I missing the obvious? 

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121220/61b91204/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


AFSA Storage Webinar

2012-11-15 Thread Bill Brooks
A little AFSA cheerleading today.

Yesterday the AFSA sponsored a webinar on storage applications.  James
Golinveaux from Tyco was the presenter. Two hours in length and worth every
penny of my membership dues. First seminar where I had outstanding
evaluation marks in every category and actually meant it. He had tables and
flow charts and detailed comparisons of NFPA 13 and FM storage rules, along
with videos. He covered the new EC applications, the 6-head designs,
cautions in making sure your open racks don't turn into solid shelving
because of slip ups in flue space allocation, etc.

Just like George Church says, membership is a great idea.  I'm in.

Bill Brooks


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Pipe support spacing requirements for structural supports

2012-11-10 Thread Bill Brooks
I definitely don't agree with this. Pipe racks are routinely installed in
industrial settings and are used for transiting roadways and other parts of
industrial sites.  The piping on these racks is designed by folks who use
standards other than NFPA 13.  I would recommend using the equivalency
provisions of Section 1.5 in this case and allowing the piping professionals
the ability to provide the calculations needed.  Sometimes we lose sight of
this important provision.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports

If the spacing of pipe rack supports does not meet the spacing requirements
of the NFPA Standards you need to supplement with intermediate hangers in
order to have a compliant installation.  I just don't use what's given.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
rfletc...@aerofire.com
Sent: Thursday, November 08, 2012 9:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports

I agree that you would have to follow NFPA 13/15 hanger requirements for
spacing of pipe stands you are building to support pipe around like a pump
set or a transformer. In the pipe rack however I think you can only use what
you are given. In the past we have used flanges to join bulk pipes in the
rack. Threaded branchlines hold up okay with hangers every 20 ft. Of course
we did all of this back before the scientists got involved in NFPA 13 so if
it was solid, wouldn't wiggle if pulled on, didn't fall down from its' own
weight and didn't move when flow tested it was good enough.

Ron Fletcher
Aero -Phoenix

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 7:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports

Whether it's a pipe stand, a hanger or pipe rack, they must conform to the
spacing requirements of the applicable standard.  NFPA 15(2012) 5.6 defers
to NFPA 13 for hangers.  I can't find any A10.4.1 in NFPA 15, 2012.  

So no, 20' hanger spacing is not compliant with the NFPA 13 or NFPA 15
standards.  The assertions of the structural engineer are incorrect.

Additionally,  I would suggest looking at the installation manuals provided
by the coupling manufacturers to see if they refer to any particular support
spacing requirements if there is specific direction needed.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Hinson, Ryan
Sent: Tuesday, November 06, 2012 7:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe support spacing requirements for structural supports

I've got a couple projects which have pipe racks for supporting above grade
firewater piping.  These rack supports are spaced at 20' or more on center.
From the NFPA 13 Handbook at the beginning of Chapter 9, pipestands are to
have the same safety factors as hangers.  NFPA 15 is suggested for
additional guidance.  NFPA 13 limits hanger spacing to 15'.  NFPA 15 (2012)
Sections 6.3.2.2 and 6.3.2.3 state that firewater piping shall be supported
under fire conditions and shall be supported from steel or concrete
structural members or pipestands.  Do these also need to conform to the 15
ft maximum spacing?

I've received this question from a structural engineer regarding the pipe
support requirements for NFPA 13 (2010) Chapter 9.  His assertion is that
this refers to pipe stand and pipe hanger spacing requirements for piping 8
and smaller only.  As such, his feeling is that there are no limits on
spacing for concrete and steel support conditions other than those required
per AWWA M11 4th Edition Chapter 7 and sound structural engineering design.
Incidentally, NFPA 15 (2012) Section 6.3.2.2 calls out structural supports
specifically as if there is some difference for their design and does not
actually provide a limit.

Both NFPA 20 (2010) Section 4.13.5 and NFPA 24 (2010) Section

Qualified NFPA 25 Persons

2012-10-17 Thread Bill Brooks
What are the qualifications for an NFPA 25 sprinkler system inspector?
Seems pretty open ended to me. We routinely look for NICET qualifications
for designers but what about the inspectors?  I'm trying to establish a
specification for NFPA 25 inspections and originally thought I'd say
qualified persons per NFPA 25 but now I'm not so sure.  Is there a NICET
program focused on inspections?

Thank you.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Draft curtain

2012-09-20 Thread Bill Brooks
See 2009 International Fire Code for some guidelines/requirements before you
confirm the depth of the curtain or the construction. Just using this
reference as an example since you didn't specify the applicable code in this
jurisdiction.  I don't think the cover on both sides is necessary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Byron Weisz -
Cen-Cal Fire Systems
Sent: Thursday, September 20, 2012 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

That is a Building Code issue

Byron Weisz
 
Cen-Cal Fire Systems, Inc.
1615 So. Stockton St. 
Lodi, CA. 95240
Ph.   (209) 334-9119
Fax   (209) 334-2923
by...@cen-calfire.com
 
This message is intended only for the use of the individual or entity to
which it is addressed and may contain information that is privileged and/or
confidential. If you are not the intended recipient any use, dissemination,
distribution, or copying of this communication and attachments is strictly
prohibited. Thank you.
 
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 8:50 AM
To: sprinklerforum@firesprinkler.org
Subject: Draft curtain
Importance: High

We have a project that we are demo'ing a pipe schedule system and installing
a ESFR system for storage. There is an adjacent area of the building that
will have a pipe schedule system w/standard response sprinklers in it. Per
NFPA13 2007 8.4.6.4 the owner will provide a draft curtain since a wall is
out of the question in this area. The draft curtain will be 2'-0 down from
the deck constructed of non-combustible materials and sealed at the deck
(probably smoke caulk). The owner is going to provide a 4'-0 clear aisle
centered on the curtain (2'-0 each way). The contractor plans on using metal
studs and roof decking material for the curtain. The question is, do the
studs have to be covered each side or is putting the decking on one side
sufficient? I didn't see anything as far as thickness of curtain or that
would lead me to believe it would have to be covered each side. 

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 http://www.keyfireprotection.com www.keyfireprotection.com

 

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120920/20d1b142/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Draft curtain

2012-09-20 Thread Bill Brooks
Table 910.3 and Section 910.3.5 of the 2006 International FIRE Code if this
is adopted.  It notes the ESFR to non-ESFR boundary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 12:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

Thank you - 2006 IBC - do you know the label of the section its in - I
glanced and didn't see it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 11:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

See 2009 International Fire Code for some guidelines/requirements before you
confirm the depth of the curtain or the construction. Just using this
reference as an example since you didn't specify the applicable code in this
jurisdiction.  I don't think the cover on both sides is necessary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Byron Weisz -
Cen-Cal Fire Systems
Sent: Thursday, September 20, 2012 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

That is a Building Code issue

Byron Weisz
 
Cen-Cal Fire Systems, Inc.
1615 So. Stockton St. 
Lodi, CA. 95240
Ph.   (209) 334-9119
Fax   (209) 334-2923
by...@cen-calfire.com
 
This message is intended only for the use of the individual or entity to
which it is addressed and may contain information that is privileged and/or
confidential. If you are not the intended recipient any use, dissemination,
distribution, or copying of this communication and attachments is strictly
prohibited. Thank you.
 
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 8:50 AM
To: sprinklerforum@firesprinkler.org
Subject: Draft curtain
Importance: High

We have a project that we are demo'ing a pipe schedule system and installing
a ESFR system for storage. There is an adjacent area of the building that
will have a pipe schedule system w/standard response sprinklers in it. Per
NFPA13 2007 8.4.6.4 the owner will provide a draft curtain since a wall is
out of the question in this area. The draft curtain will be 2'-0 down from
the deck constructed of non-combustible materials and sealed at the deck
(probably smoke caulk). The owner is going to provide a 4'-0 clear aisle
centered on the curtain (2'-0 each way). The contractor plans on using metal
studs and roof decking material for the curtain. The question is, do the
studs have to be covered each side or is putting the decking on one side
sufficient? I didn't see anything as far as thickness of curtain or that
would lead me to believe it would have to be covered each side. 

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 http://www.keyfireprotection.com www.keyfireprotection.com

 

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120920/20d1b142/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2221 / Virus Database: 2441/5281 - Release Date: 09/20/12

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Draft curtain

2012-09-20 Thread Bill Brooks
I see an Exception from the area requirements of Table 910.3 but there is no
exception from the need to separate ESFR from conventional.  So when there
is a need for a draft curtain there would be a minimum 4 ft depth.  Perhaps
someone can help me with this.  I am not involved with storage 24/7.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

Thank you both. I did mean IFC Bill - thank you. The only reason for the
draft curtain is due to the different response elements of the sprinklers as
Chris said. Looking at IFC 2006 910.3.5 it appears my situation qualifies
for the Exception and I can apply the 2'-0 depth as referenced in NFPA13
2007 8.4.6.4. It will be smoke tight.

Thanks again. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 12:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

Table 910.3 and Section 910.3.5 of the 2006 International FIRE Code if this
is adopted.  It notes the ESFR to non-ESFR boundary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 12:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

Thank you - 2006 IBC - do you know the label of the section its in - I
glanced and didn't see it.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, September 20, 2012 11:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

See 2009 International Fire Code for some guidelines/requirements before you
confirm the depth of the curtain or the construction. Just using this
reference as an example since you didn't specify the applicable code in this
jurisdiction.  I don't think the cover on both sides is necessary.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Byron Weisz -
Cen-Cal Fire Systems
Sent: Thursday, September 20, 2012 12:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Draft curtain

That is a Building Code issue

Byron Weisz
 
Cen-Cal Fire Systems, Inc.
1615 So. Stockton St. 
Lodi, CA. 95240
Ph.   (209) 334-9119
Fax   (209) 334-2923
by...@cen-calfire.com
 
This message is intended only for the use of the individual or entity to
which it is addressed and may contain information that is privileged and/or
confidential. If you are not the intended recipient any use, dissemination,
distribution, or copying of this communication and attachments is strictly
prohibited. Thank you.
 
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, September 20, 2012 8:50 AM
To: sprinklerforum@firesprinkler.org
Subject: Draft curtain
Importance: High

We have a project that we are demo'ing a pipe schedule system and installing
a ESFR system for storage. There is an adjacent area of the building that
will have a pipe schedule system w/standard response sprinklers in it. Per
NFPA13 2007 8.4.6.4 the owner will provide a draft curtain since a wall is
out of the question in this area. The draft curtain will be 2'-0 down from
the deck constructed of non-combustible materials and sealed at the deck
(probably smoke caulk). The owner is going to provide a 4'-0 clear aisle
centered on the curtain (2'-0 each way). The contractor plans on using metal
studs and roof decking material for the curtain. The question is, do the
studs have to be covered each side or is putting the decking on one side
sufficient? I didn't see anything as far as thickness of curtain or that
would lead me to believe it would have to be covered each side. 

 

Thank you,

 

Bobby Gillett

Sr

RE: Ventilation for diesel driven fire pump room

2012-08-24 Thread Bill Brooks
I've consulted with Tigerflow in the past on projects requiring standalone
fire pump enclosures.  They ship worldwide and I'm sure they would accept a
phone call to discuss this if you do not have access to a mechanical
engineer (HVAC type) who does this routinely.

As others have noted the engine needs combustion air and the pump room may
require supplemental cooling (or heating).  Depending on how the room is
classified by the Mechanical code, a minimum ventilation rate could be
required as well.  Generally, if not considered occupied, there would be
no ventilation requirement (see 2009 International Mechanical Code, 401.2)
but your jurisdiction's code may be amended in some way.  I suppose the size
of the room is not the controlling factor if the only requirement is for the
pump driver combustion air.  For supplemental cooling this would matter when
calculating heat loss/gain through the enclosure.

www.tigerflow.com

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David Bitton
Sent: Thursday, August 23, 2012 6:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Ventilation for diesel driven fire pump room

Where I can find guidelines for determining the size of the ventilation
openings in a pump room containing a diesel-engine driven pump? I imagine
that the size would depend on the room size (volume) and the size of engine.


 

David Bitton, ing.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120823/efe19989/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Ventilation for diesel driven fire pump room

2012-08-24 Thread Bill Brooks
Google search result for combustion air requirements diesel engine

http://www.cumminsfirepower.com/documents/ES027_ventilation.pdf

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David Bitton
Sent: Thursday, August 23, 2012 6:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Ventilation for diesel driven fire pump room

Where I can find guidelines for determining the size of the ventilation
openings in a pump room containing a diesel-engine driven pump? I imagine
that the size would depend on the room size (volume) and the size of engine.


 

David Bitton, ing.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120823/efe19989/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: solid shelves in auto parts stores

2012-08-16 Thread Bill Brooks
Anytime the word storage appears there's a need for much more extensive
analysis of all of the likely materials and their configuration. For example
the 2009 International Fire Code deals with retail storage of aerosols in
Section 2806 with 8 ft and 8 ft categories.  Flammable and combustible
liquids are covered in IFC 3404.4. Then there are the Group A plastics
determined by the product itself or the packing material covered in IFC
Chapter 23.  Note the definition of high-piled high-hazard commodities could
start at 6 ft.

Ceiling height was not noted.  This could dictate maximum storage height.

Without looking at any further I'd say the chance of OH2 would be slim.

Looks like NFPA 13 is applied for the shelf storage question per IFC Section
2307.

Maybe this major chain store already has corporate guidelines.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, August 16, 2012 3:30 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: solid shelves in auto parts stores

Considering the amount of rubber and plastic parts, oil, solvents and
aerosol sprays and paint, I think it should be higher. I think in spots it
is more than a class 4 commodity. 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:14 PM
To: sprinklerforum@firesprinkler.org
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30 deep in this scenario without
protection in the racks?

Is OH@ appropriate for these typical Auto Parts Stores with the storage as
it is?

Thanks for your help if you have time, if not please ignore and have a great
day!




--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com 1160
McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120816/ec9499ea/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5203 - Release Date: 08/15/12

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: solid shelves in auto parts stores

2012-08-16 Thread Bill Brooks
From a sign-off responsibility standpoint, it seems like it could be
approved.

Maybe, but only if you provide a letter stating the owner is responsible for
storage arrangement and contents complying with NFPA 13 (2007), Table 13.2.1
for OH2 design. But, then again, all this information would already be
stated in the Owner's Certificate. (??)

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Thursday, August 16, 2012 5:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: solid shelves in auto parts stores

Is there any reason why this would not meet the letter of the code for OH2
protection of a mercantile application?

If questions are going to be raised about if they will stack over 12' on 12'
racks, one might also wonder if they will change the racks out for taller
racks, etc. Wouldn't the design have to be based on the stated intent for
the tenant?

I agree that this is probably on the high side of what OH2 was intended for.
It could also be protected by the retail storage criteria (NFPA 13 2007
20.3). If I was their insurance carrier, I might be more concerned.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, August 16, 2012 4:03 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: solid shelves in auto parts stores

Anytime the word storage appears there's a need for much more extensive
analysis of all of the likely materials and their configuration. For example
the 2009 International Fire Code deals with retail storage of aerosols in
Section 2806 with 8 ft and 8 ft categories.  Flammable and combustible
liquids are covered in IFC 3404.4. Then there are the Group A plastics
determined by the product itself or the packing material covered in IFC
Chapter 23.  Note the definition of high-piled high-hazard commodities could
start at 6 ft.

Ceiling height was not noted.  This could dictate maximum storage height.

Without looking at any further I'd say the chance of OH2 would be slim.

Looks like NFPA 13 is applied for the shelf storage question per IFC Section
2307.

Maybe this major chain store already has corporate guidelines.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, August 16, 2012 3:30 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: solid shelves in auto parts stores

Considering the amount of rubber and plastic parts, oil, solvents and
aerosol sprays and paint, I think it should be higher. I think in spots it
is more than a class 4 commodity. 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Thursday, August 16, 2012 3:14 PM
To: sprinklerforum@firesprinkler.org
Subject: solid shelves in auto parts stores

Hello,

1) There is a PE involved
2) This is not my job, but I am trying to be a friend to the AHJ'
3) I can't readily put my hands on this due to other issues


A local AHJ has called me to inquire about the requirement for protecting a
major chain Auto Parts Store. The PE has stated OH2 throughout the store.
AHJ is asking questions because there are 12' tall racks with a solid top
making him think they will store over 12'.

Questions,

Are solid shelves allowed in racks aver 30 deep in this scenario without
protection in the racks?

Is OH@ appropriate for these typical Auto Parts Stores with the storage as
it is?

Thanks for your help if you have time, if not please ignore and have a great
day!




--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com 1160
McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120816/ec9499ea/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-
No virus found in this message

RE: 02 storage (hazardous materials assessment)

2012-08-13 Thread Bill Brooks
The definition of O2 as a hazardous material is based on IBC Section 307.2
and the defined quantities in IBC Table 307.1(1).  When quantities exceed
the MAQ in Table 307.1(1), the various design options being discussed come
into play.  The concept of Control Area is defined in (2009) IBC Section
414.2. The IBC fire barrier is noted in Table 414.2.2.

I'm very surprised any AHJ would have to be educated on this, but looking
back at the messages it may be that what the AHJ said was being filtered
through a number of people who were not familiar with the process used to
deal with hazardous materials.

What I've found in the real world is the lack of correlation between
commonly generated MSDS and the various building and fire code
classification tables which does not appear to factor into this application.

I'm not familiar with the Florida Building Code, perhaps it is much more
complex than the IBC.

Keep in mind there are 13 Exceptions listed under Section 307.1, one of
which (Exception 2) is the storage of flammable and combustible liquids in
mercantile. If it were not for this exception some stores we regularly shop
in would not exist in their present form. Also Exception 6 is your
neighborhood State Store (a nod to George C.).

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Friday, August 10, 2012 3:05 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 02 storage

Sounds like there are some building code issues which should not be
addressed by the sprinkler contractor. It may be your job is not so
complicated if you apply NFPA 55.  But somebody else may or may not have
done their job.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
jhoff...@kcp.com
Sent: Friday, August 10, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: 02 storage

IFC, chapter 27 and NFPA 55 have the same criteria for oxidizing gas.  It is
3000 cu ft per control area.  Don't know where the AHJ is coming up with
12000 cu ft unless he is considering the maximum of 4 control areas per
building and then you get to 12000 cu ft.  This means 4 areas that are fire
separated from each other and the rest of the building.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns  McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FMT |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
jhoff...@kcp.com



From:   Greg McGahan g...@livingwaterfp.com
To: sprinklerforum@firesprinkler.org
Date:   08/10/2012 12:50 PM
Subject:02 storage
Sent by:sprinklerforum-boun...@firesprinkler.org



This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is having
difficulty with the AHJ who claims that even if they classify the warehouse
portion of this space as Storage Occupancy instead of Business, The maximum
cubic footage of 02 allowed to be stored in one place is 12,000 with High
Hazard Sprinkler protection. The tenant needs to store almost 20,000 cubic
feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120810/f3e9c5a0/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: 02 storage

2012-08-10 Thread Bill Brooks
Sounds like there are some building code issues which should not be
addressed by the sprinkler contractor. It may be your job is not so
complicated if you apply NFPA 55.  But somebody else may or may not have
done their job.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
jhoff...@kcp.com
Sent: Friday, August 10, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: 02 storage

IFC, chapter 27 and NFPA 55 have the same criteria for oxidizing gas.  It is
3000 cu ft per control area.  Don't know where the AHJ is coming up with
12000 cu ft unless he is considering the maximum of 4 control areas per
building and then you get to 12000 cu ft.  This means 4 areas that are fire
separated from each other and the rest of the building.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns  McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FMT |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
jhoff...@kcp.com



From:   Greg McGahan g...@livingwaterfp.com
To: sprinklerforum@firesprinkler.org
Date:   08/10/2012 12:50 PM
Subject:02 storage
Sent by:sprinklerforum-boun...@firesprinkler.org



This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is having
difficulty with the AHJ who claims that even if they classify the warehouse
portion of this space as Storage Occupancy instead of Business, The maximum
cubic footage of 02 allowed to be stored in one place is 12,000 with High
Hazard Sprinkler protection. The tenant needs to store almost 20,000 cubic
feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120810/f3e9c5a0/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI Cloud Deluge

2012-06-07 Thread Bill Brooks
Yes we have a rulebook instead of an engineering approach (thank goodness),
and yes we have been fumbling around for many years about this cloud thing,
but in the name of common sense (which I hope we still have a little of)
this design approach must be stopped at all costs.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike
Hairfield
Sent: Wednesday, June 06, 2012 3:36 PM
To: AFSA SprinklerFORUM
Subject: RE: RTI


You won't believe this!
 
Armstrong ceiling clouds that are arched, architect doesn't want to
penetrate the clouds like the Armstrong data sheet shows so we have QR
sprinklers above the clouds and a deluge system of sidewall sprinklers feed
from the soffits throwing water under the clouds. Some big DA came up with
this idea.
 
It's a tiered classroom with a sloping floor, I suggested they install some
life preservers for the students so they won't drown when the system trips.
 
Mike
 

 

 From: craig.pr...@ch2m.com
 To: sprinklerforum@firesprinkler.org
 Subject: RE: RTI
 Date: Wed, 6 Jun 2012 19:29:07 +
 
 Are the detectors at the same temperature as the QR heads? That just sound
weird, what would be in the same room that would be protected by deluge
system and also allow QR sprinklers?
 
 Craig L. Prahl, CET
 Fire Protection
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension 74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
 Hairfield
 Sent: Wednesday, June 06, 2012 2:08 PM
 To: AFSA SprinklerFORUM
 Subject: RE: RTI
 
 
 There are QR Sprinklers in the same room that has a deluge system with 
 open heads in it, they want to make sure that the detectors do not trip
the deluge system first.
 
 
 
 
  From: ccah...@burnsmcd.com
  To: sprinklerforum@firesprinkler.org
  Date: Wed, 6 Jun 2012 12:31:18 -0500
  Subject: RE: RTI
  
  Curious if you know why the AHJ wanted to know? Listings take care of
either FR/QR or SR. 
  
  Chris Cahill, PE*
  Senior Fire Protection Engineer, Aviation  Facilities Group Burns  
  McDonnell
  8201 Norman Center Drive
  Bloomington, MN 55437
  Phone: 952.656.3652
  Fax: 952.229.2923
  ccah...@burnsmcd.com
  www.burnsmcd.com
  
  Proud to be one of FORTUNE's 100 Best Companies to Work For 
  *Registered in: MN
  
  
  
  
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org 
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
  Hairfield
  Sent: Wednesday, June 06, 2012 12:26 PM
  To: AFSA SprinklerFORUM
  Subject: RE: RTI
  
  
  Thanks,
  
  They told me it was 36.
  
  Mike
  
  
   From: craig.pr...@ch2m.com
   To: sprinklerforum@firesprinkler.org
   Subject: RE: RTI
   Date: Wed, 6 Jun 2012 17:21:17 +
   
   Call Tyco.
   
   
   Craig L. Prahl, CET
   Fire Protection
   CH2MHILL
   Lockwood Greene
   1500 International Drive
   Spartanburg, SC 29304-0491
   Direct - 864.599.4102
   Fax - 864.599.8439
   CH2MHILL Extension 74102
   craig.pr...@ch2m.com
   
   
   
   -Original Message-
   From: sprinklerforum-boun...@firesprinkler.org
   [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
   Mike Hairfield
   Sent: Wednesday, June 06, 2012 1:19 PM
   To: AFSA SprinklerFORUM
   Subject: RTI
   
   
   I have a AHJ wanting to know what is the RTI for a TYCO FR-B TY3231
155 degree pendent sprinkler.
   
   How do I determine the RTI?
   
   Mike
   -- next part -- An HTML attachment was 
   scrubbed...
   URL: 
   http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
   atta chments/20120606/0ddfb8a7/attachment.html
   ___
   Sprinklerforum mailing list
   Sprinklerforum@firesprinkler.org
   http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
   ___
   Sprinklerforum mailing list
   Sprinklerforum@firesprinkler.org
   http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
  -- next part -- An HTML attachment was 
  scrubbed...
  URL: 
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
  tachments/20120606/47d8575c/attachment.html
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman

RE: minimum 7 PSI end head logic, check please!

2012-06-04 Thread Bill Brooks
What are you comments with regard to Figure 11.2.3.2.3.1 (2010)?

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Monday, June 04, 2012 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: minimum 7 PSI end head logic, check please!

Thanks Mark,
I would not want to reduce LH spacing. I think density should be tied to
sprinkler height and area to occupancy. I think the water demands are too
high for low ceilings and too low for high ceilings. Basing min flow rate on
density time head area, without min end head PSI brings the demand down
where the ceiling heights are less that 12'-6. Activation time is a
function of ceiling height and is the main reason for tieing density to it
too.

thanks again,
Brad

-Original Message-
From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
Sent: Monday, June 04, 2012 7:30 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: minimum 7 PSI end head logic, check please!

Research the development history of the Residential  sprinkler. It was done
during the late 70's and covered all the issues you're thinking about here.
I believe NFPA 13D was first published in 1980 or '81. I think I remember
that some of the first heads listed for residential had a minimum starting
pressure of 5 PSI. I know there were design densities of .05 GPM/PSF. Also
the residential Sprinkler is designed to hit the WALL near the ceiling at
minimum operating pressure. Just out of curiosity, why would you want to
reduce LH spacing to 100 Sf?
Mark at Aero

- Original Message -
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
Sent: Monday, June 04, 2012 06:57 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: minimum 7 PSI end head logic, check please!

Good points guys, thanks. Here is an 'equivalency thought experiment' if the
Forum will suffer me a little more: the water hits the floor (at a wall 9'
away when it has 7 PSI on it. Throttle the flow down until it hits the floor
5' away. Now what is the pressure? We don't know until we measure it, but
for 100 s.f. head spacing it is obviously less than 7 PSI. I am not trying
to rock the boat or waste anyone's time. I plan on submitting a proposal for
change regarding calc rules for water supplies for LH and OH, so I am trying
to establish equivalency, identify arbitrariness, etc. Is it coincidence
that 7 PSI is 32 ft/sec? I only got 20 years to get this change through so I
thought I'd better get started.

-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Sunday, June 03, 2012 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: minimum 7 PSI end head logic, check please!

Oops, forgot the pattern part (thanks Bruce), but the argument is the same.
The head is tested/listed at not less than psi. Rule 1 then is 7 psi or
more, if less than 7 psi raise the starting pressure to 7 psi, that's it,
don't worry, carry on, complete the design, get it out the door, and
approved, build-it, get it signed off, collect the money, move on.

On Sun, Jun 3, 2012 at 1:36 PM, Bruce Verhei bver...@comcast.net wrote:

 Would the heads make an effective pattern below 7psi, and more 
 important, is the answer known, and not guessed at?

 Bruce

 Sent from my Motorola ATRIXT 4G on ATT

 -Original message-
 From: bcasterl...@fsc-inc.com
 To: sprinklerforum@firesprinkler.org
 Sent: Sun, Jun 3, 2012 20:31:30 GMT+00:00
 Subject: minimum 7 PSI end head logic, check please!

 Fact: a minimum pressure is required to 'push the stopper out of the 
 orifice' once the 'link has broken'. This means the column of water 
 above the head has to be at least 16 feet tall. (i wonder if this is 
 enough for the 'bigger stoppers' of today, but I'll trust the 
 manufacturers). An overall statement could be made Sprinklers do not 
 work where the static
is
 less than 7 PSI.
 Question: Why should we calculate the minimum required flow rate based 
 on anything other than density times head area, since at that point 
 the stopper has already been pushed out?
 If in doubt about the Pt available to a non-flowing head when others 
 are flowing, couldn't we use a flow test graph to find GPM at 7 PSI, 
 and make sure we are flowing less than that?

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 

http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120603/c7182724/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates

Adjusting Pump Curves for Pump Speed

2012-05-09 Thread Bill Brooks
This is something I should know, but how are pump curves adjusted for pump
speed?  I'm looking at a curve based on 3450 rpm (60 Hz) and want to adjust
it for 2900 rpm (50 Hz).  Is this possible?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Adjusting Pump Curves for Pump Speed

2012-05-09 Thread Bill Brooks
Thanks, age is a good thing in some products, but ...

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Wednesday, May 09, 2012 12:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Adjusting Pump Curves for Pump Speed

See NFPA 20, A.14.2.5.4(7)(f) on page 90 of the 2010 ed.


Steve Leyton




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Wednesday, May 09, 2012 9:11 AM
To: sprinklerforum@firesprinkler.org
Subject: Adjusting Pump Curves for Pump Speed

This is something I should know, but how are pump curves adjusted for pump
speed?  I'm looking at a curve based on 3450 rpm (60 Hz) and want to adjust
it for 2900 rpm (50 Hz).  Is this possible?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Water testing volumes

2012-04-23 Thread Bill Brooks
And almost exactly 500 gpm for 20 minutes.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 23, 2012 8:55 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water testing volumes

Have you asked the owner the purpose of the tank?

Sounds like a secondary containment tank.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Friday, April 20, 2012 3:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water testing volumes

 
In an industrial building there is a concrete storage tank below gound
level. It is about 19'x7' and 10 feet deep and covered with an open grated
steel panel. Top of the steel panel is level with the adjacent ground floor
level. Someone said it was to collect rain water but I need to get that
confirmed. It could even be that the other floor drains drained into this
tank and was pumped out. Anyway, this space is non-combustible, but could
collect debris that would fall through the open grate panel. The question
is, does it have to be sprinklered? I would say NO, but is there anything in
the code to justify that position?

Tony   

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: UFC3-600-01

2012-04-05 Thread Bill Brooks
You may also have a 25 year system life on your job, and this may not be
incorporated into the sprinkler specification.  It may be in the boiler
plate that's in the hands of the general contractor, and it may not have
been passed along to you.  I believe the sprinkler system would be one of
the elements that would have to meet this life span.  In my experience this
particular requirement is not well understood by anyone on the design side,
the contracting side, or the owner.  Whatever you do you better make it
clear what you intend to provide.  The standard use schedule 40 may not be
applicable for aggressive water conditions if the Sched. 40 pipe won't last
25 years.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Stough
Sent: Thursday, April 05, 2012 2:43 PM
To: sprinklerforum@firesprinkler.org
Subject: UFC3-600-01

Thanks. I had not had anyone ask about MIC in so long, I forgot about it. 
Is anyone testing for MIC and finding anything?  In the last two years,
we've tested 8 systems and only 1 had the possibility of bacterial growth.

 
Jay Stough



 From: etamb...@aerofire.com etamb...@aerofire.com
To: sprinklerforum@firesprinkler.org 
Sent: Thursday, April 5, 2012 1:54 PM
Subject: RE: UFC3-600-01
 
We had a similar comment come up on a USACE project and we were allowed to
get a letter from the local fire marshal saying that there have been no
historical problems with piping corrosion in their district.

Ed
AERO Automatic Sprinkler Company
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120405/e6c0d21d/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Bill Brooks
Common practice in my experience is to list these flows as part of the
contract documents and then require the winning contractor to conduct a
confirming flow test prior to submitting drawings and calculations.  I
assume you've accounted for elevation in your example in that the
static/residual hydrant is at the same elevation as the BOR.  But I'm not
saying I would list these flows or issue this documentation as you've
described.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available! Can contractors arbitrarily
choose curves to meet their design needs, can interpreted points on a graph
such as those used in test two be used over real numbers such as those in
test three? My gut tells me no, but it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: FM 74 Egress Sprinklre system?

2012-03-26 Thread Bill Brooks
NFPA 101A has a number of partial sprinkler system options for various
occupancies.  I recall the original development of the point systems in the
late 1970's where partial systems were given consideration in life safety
evaluations.  Perhaps the system in this case is a holdover from that time
period.  It would be instructive to take a look at past and current versions
of NFPA 101A to see how some of these systems could have been introduced
especially on the fire marshal side where NFPA could have been used in lieu
of building codes in upgrading existing buildings.  NFPA 101 has included a
provision for 6 heads off domestic for many years. 

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Sunday, March 25, 2012 5:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: FM 74 Egress Sprinklre system?

Douglas,

During the early eighties and maybe the seventies (I was in California until
the late eighties so I'm not sure about the when) schools K-12 were under
the jurisdiction of the State FM. There were several I've come across with
these silly partial systems protecting small areas deemed to be extra
dangerous for one reason or another, including the main building at Bates
Tech College (which was a vocational adult school in the Tacoma school
District until 1988), my own institution. In the entry to what is now the
financial aid office, but then was registration, are seven Omega heads over
the doorway. There are four along one wall in a counselor's office but that
wall used to be a pass through of some sort with a drop window arrangement.
There's an elementary school in Puyallup with two heads (and six spares)
covering a stage (platform), and a high school with four heads over the
main office counter (highly combustible paperwork no doubt).
All these systems are tapped off plumbing, and installed in, at best, a
pipe schedule, or to nothing cogent at all like your system seems to be.
I wouldn't be surprised if Washington nonsense migrated to Oregon. You may
be looking at something somebody thought was a good idea at the time,
like that six month or so surge of a single sprinkler head over a
residential cooking surface tapped off the plumbing. Or perhaps tose guys
that decided if some anti-freeze was good 100% anti-freeze would be better,
until

On Sun, Mar 25, 2012 at 12:59 PM, Douglas Hicks fire...@eoni.com wrote:

 I am looking at 2 schools that have partial sprinkler systems, 
 protecting the egress routes only.  The local Fire Marshal thinks they 
 may be installed to FM74 standards.  The 2 that I have seen are wet 
 systems, 1/2 inch drops to the heads, 1/2 garden hose fitting as an
inspector's test.
 The heads are pendant, and uprights,  as far  as 2 feet from the ceiling.
 Some of the heads are leaking, some of the heads look to be oriented 
 improperly. No one seems to know what the year of installation was.  
 Is/was there a standard for that type of sprinkler system?
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
 hments/20120325/0cd46534/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120325/fb7364e8/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Radiation Vaults

2012-03-23 Thread Bill Brooks
The penetration arrangement has a lot to do with the location or possible
locations of a source material.  At times the 45 isn't sufficient and an
offset is needed so that there is no straight line of sight from the inside
to the outside.  Sometimes this is difficult to deal with when the wall is
36 thick and your penetration has not been incorporated into the
construction ahead of time.  In other cases a radiation area may be
maintained negative pressure and these penetrations would require special
sealing.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Friday, March 23, 2012 1:31 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radiation Vaults

Thank you! 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Randy Knutson
Sent: Friday, March 23, 2012 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radiation Vaults

Bobby,
The only strange thing that I encountered was that all penetration through
the vault had to be at 45º angle. Our sleeves were provided by others. Other
than that it was a wet-pipe system with Sch 40 pipe  DI fittings.

Randy Knutson
Shilo Automatic Sprinkler, Inc.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, March 22, 2012 7:57 AM
To: mi...@phoenixfp.net; sprinklerforum@firesprinkler.org
Subject: RE: Radiation Vaults

Thank you for your response. They did not spec anything special other than
the pre-action, that is just for safety factor I am sure. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hill
Sent: Thursday, March 22, 2012 8:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radiation Vaults

I have done a few of these. None required a preaction system. Black pipe was
acceptable for the wet systems that we installed. There is usually only one
penetration into the room. There were no special requirements for the
penetrations on the ones I did (no dielectrics or wave guides)

Mike Hill


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett
Sent: Thursday, March 22, 2012 9:33 AM
To: sprinklerforum@firesprinkler.org
Subject: Radiation Vaults

We are bidding a project that has Linear Accelerator Vaults. These areas
have thick concrete walls, floor and ceilings and the machine produces
radiation for cancer treatment. They spec us installing D.I. Preaction
systems for these vaults. Is anyone familiar with these? My question is can
we use black steel pipe and do we have to do anything special at our
penetrations into the rooms?

 

Thank you in advance.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 http://www.keyfireprotection.com www.keyfireprotection.com

 

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120322/57a64e9f/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4885 - Release Date: 03/21/12

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 9.0.0.909, Virus/Spyware Database: 6.19510)
http://www.pctools.com/
===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 9.0.0.909, Virus/Spyware Database: 6.19520)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-
No virus

RE: 52,000 square feet

2012-01-06 Thread Bill Brooks
NFPA 13, 1.5 (2007) requires TECHNICAL documentation.  I believe you must
demonstrate equivalency.  Would it be water flow alarm is just as fast?
Would it be that fire control is comparable?  Would it be that overall
reliability is the same?  The first can be answered by timing the signal
with the bigger system, the second could be answered by submission of
hydraulic calculations, but the third is unanswerable unless you and the
rest of us know what factors went into the 52,000 sq ft requirement in the
first place.  We all know it's OK to have a single valve control 52,000 sq
ft of LH/OH system, but at 52,001 sq ft you are not equivalent.I don't
see how any of the factors you seem to have come up with will do that.
You're actually asking for a Modification as described in IBC 2009, 104.10.
Then perhaps your reasons have some merit and could be accepted.  But then
again the language of 104.10 brings in the term does not lessen. 

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Friday, January 06, 2012 3:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: 52,000 square feet

Follow up -

I posed this question to the EOR and the AHJ. The AHJ has a good friend in
another part of the state who looked at it from a 3rd party objective point
of view and stated that because:

1) this is a school occupied only during the day and the School Board policy
is that all system shut downs occur when the building is unoccupied or at
least when no students are present
2) the building is non-combustible with fire rated corridors and classrooms
( a lot of passive protection)
3) there is complete Fire Alarm System in place

He would absolutely have no problem enlarging the system size. The local EOR
said he was fine with it as well due to the fact that the existing system
configuration does not lend itself to restructuring a portion near the riser
( inorder to reduce the existing systems size enough to add on the other
ends) without major  renovations and that he wants to keep the wings on the
same systems for future maintenance and to negate the potential for a flood.

Therefore, it appears that we have agreement in this particular case.


Thanks for your feedback,
Greg

On Fri, Jan 6, 2012 at 2:02 PM, George Church g...@rowesprinkler.com wrote:

 Data for which one would think FM Global has, or they wouldn't have 
 relaxed their requirement to 60k without technical substantiation.
 Hopefully someone up there will write a proposal sharing enough of 
 that data so the 13 TC can consider addressing a change in the system
area.

 One would think it would be prudent to consider the propensity for a 
 building's occupancy to have changes made. A spec multi-tenant 
 building with 1 and 2 year leases will likely have shutdowns for 
 tenant mods often, compared to a hotel that's built, and pretty much 
 stays that way until they change the wallpaper and wall sconces every 5
years or more.

 George L.  Church, Jr., CET
 Rowe Sprinkler Systems, Inc.
 PO Box 407, Middleburg, PA 17842
 877-324-ROWE   570-837-6335 fax
 g...@rowesprinkler.com



 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:
 sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
 Sent: Tuesday, January 03, 2012 11:41 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: 52,000 square feet

 Statistically the single biggest reason for system failure is a closed 
 valve so multiple valving (zoning) is not the answer. I think the shut 
 down for maintenance system argument is the the area of spurious. What 
 are the numbers on this occurring? And although I agree with 
 limitations making some sort of sense just because without them abuse 
 occurs, I think they do need to be based on stats and per risk type 
 (as Chris suggests) rather than on how many heads the schedule (that 
 is no longer used for the most part) goes to.

 On Tue, Jan 3, 2012 at 7:53 AM, Greg McGahan g...@livingwaterfp.com
 wrote:

  It would be great if there were allowances for  systems that could 
  be subdivided so that no more than xxx sq ft is disabled at a time 
  rather than limit the entire system size.
 
  On Tue, Jan 3, 2012 at 9:38 AM, Cahill, Christopher 
  ccah...@burnsmcd.com
  wrote:
 
   I'm not sure I agree they need to go away.  I understand they 
   didn't exactly come from a well thought out principal based on 
   some scientific merit.  But my reasoning goes like this.  In a 
   208,000 sq.ft. building right now we would have 4 systems.  If a 
   system is down for maintenance
  or
   say to add a head in a new office there is a 75% chance the fire 
   will
  start
   in a sprinklered area.  And yes I have been involved with two 
   buildings where the system was off when the fire started.  Get rid 
   of the limits
  and
   there is a 100% chance the fire starts in an unsprinklered area 
   during

RE: 52,000 square feet

2012-01-03 Thread Bill Brooks
Maybe not this century but in the next we will have an NFPA process where
the committees will have to explain the rationale for the current rules
before they can be carried over from one edition to the next.  That would
certainly make for some long meetings or some brief standards.

After working at this for about 40 years I have no idea how to propose a
55,000 sq ft system using NFPA 13.  NFPA 13, 1.5 seems to make it simple
Technical documentation shall be submitted to the authority having
jurisdiction to demonstrate equivalency, but actually it's impossible if
the committee doesn't know how to do it.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
Severna Park, MD 21146-1904


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Tuesday, January 03, 2012 11:41 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: 52,000 square feet

Statistically the single biggest reason for system failure is a closed valve
so multiple valving (zoning) is not the answer. I think the shut down for
maintenance system argument is the the area of spurious. What are the
numbers on this occurring? And although I agree with limitations making some
sort of sense just because without them abuse occurs, I think they do need
to be based on stats and per risk type (as Chris suggests) rather than on
how many heads the schedule (that is no longer used for the most part) goes
to.

On Tue, Jan 3, 2012 at 7:53 AM, Greg McGahan g...@livingwaterfp.com wrote:

 It would be great if there were allowances for  systems that could be 
 subdivided so that no more than xxx sq ft is disabled at a time rather 
 than limit the entire system size.

 On Tue, Jan 3, 2012 at 9:38 AM, Cahill, Christopher 
 ccah...@burnsmcd.com
 wrote:

  I'm not sure I agree they need to go away.  I understand they didn't 
  exactly come from a well thought out principal based on some 
  scientific merit.  But my reasoning goes like this.  In a 208,000 
  sq.ft. building right now we would have 4 systems.  If a system is 
  down for maintenance
 or
  say to add a head in a new office there is a 75% chance the fire 
  will
 start
  in a sprinklered area.  And yes I have been involved with two 
  buildings where the system was off when the fire started.  Get rid 
  of the limits
 and
  there is a 100% chance the fire starts in an unsprinklered area 
  during these same down times.  Double the current limits and it's 50/50.
  Remember most work is in design build which almost always = lowest 
  bid = one system per building.
 
  Sure make the argument some places will have thoughtful engineers, 
  thoughtful contractors, or owners that are interested in issues like 
  this and I won't argue but what about the majority of work.  Modify 
  the limits perhaps but they shouldn't go away.  Maybe something like 
  warehouses
 100k,
  HPS 40k, single tenant office buildings 50k, lease office 30k, malls 
  by tenant.  By floor in lease or malls, building over 4 stories.
 
  Chris Cahill, PE*
  Senior Fire Protection Engineer
  Aviation  Facilities Group
  Burns  McDonnell
  P:  952.656.3652
  F:  952.229.2923
  ccah...@burnsmcd.com
  www.burnsmcd.com
  *Lic. in MN
 
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org [mailto:
  sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
  Sent: Tuesday, January 03, 2012 9:16 AM
  To: sprinklerforum@firesprinkler.org
  Subject: Re: 52,000 square feet
 
  These limitations need to go away. They're based on pipe schedules, 
  and not because the limitations are true , but merely because the 
  schedule stops at
  400 heads. In the days when schedules were developed 52K was a 
  really big building.
 
  On Mon, Jan 2, 2012 at 10:48 AM, Matt Grise m...@afpsprink.com wrote:
 
   Now that FM allows 60ksf, I have had more success convincing AHJ's 
   that sprinkler systems still work when they exceed 52K.
  
   Matt Grisé PE*, LEED AP
   Sales Engineer
   Alliance Fire Protection
   130 w 9th Ave.
   North Kansas City, MO 64116
  
   *Licensed in KS  MO
  
   913.888.0647 ph
   913.888.0618 f
   913.927.0222 cell
   www. AFPsprink.com
  
   -Original Message-
   From: sprinklerforum-boun...@firesprinkler.org [mailto:
   sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd - FPDC
   Sent: Monday, January 02, 2012 12:46 PM
   To: sprinklerforum@firesprinkler.org
   Subject: Re: 52,000 square feet
  
   Chris, I agree is that is what the Code says. However, the 52000 
   is an arbitrary number and has no real impact on protection. For a 
   couple of thousand square feet, I wouldn't have a big problem
suggesting it.
   Probably 3k max.
  
   Sent from my iPhone
  
   On Jan 2, 2012, at 12:46 PM, Cahill, Christopher
   ccah...@burnsmcd.com
   wrote:
  
As a former AHJ many requests, all denied with I agree it's 
silly but
   it's the law

Ultrasonic Flow Meters

2011-10-28 Thread Bill Brooks
I have a special situation where I'll be testing pumps on a combined
domestic/fire water supply.  Water is in a ground level tank, multiple pumps
blue arranged to start sequentially as demand increases.  Some of these
blue pumps are designated as fire pumps and have higher flow
characteristics.  Problem is there is no test header and the testing will
have to be performed without shutting down the water system.

My suggestion is to do the testing at a low demand period but use clamp-on
type flow measuring devices at the pump discharge.  Compare the hydrant flow
to the ultrasonic flow to identify the simultaneous domestic demand +
leakage.  When I contacted FM about this they did not have any objection to
this technology but said no manufacturer had ever submitted this technology
for approval.  I know it's common in the industrial setting but I am
wondering if any of you red pump people have ever come across an
application?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Underground Main Pressure Test

2011-10-14 Thread Bill Brooks
It's been many years since I've witnessed an underground pressure test.
What is the current practice for testing a 1000+ ft length of underground?
Positive displacement pump?  How to measure the amount of water added?

Any help would be appreciated.

(All messages from George Church to the forum get snagged by my Trend Micro
- please don't be tempted to turn this into a series of with George's
reputation it's surprising it hasn't happened a long time ago responses)

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


13R in Residential (Confession)

2011-09-12 Thread Bill Brooks
My previous opinion on the use of 13R in mixed occupancy buildings was based
on incorrect information.  What I didn't know was that the text of the 2009
IBC (First Printing Feb 2009) 903.3.1.2 was changed by an Errata.  I'm a
little embarrassed in not knowing this before I posted my I'm 100% right
opinion on the matter.  For those of you who bought the early printing of
the 2009 IBC, this change may clear up some of the confusion.

What is true is that contractors bidding 13R in a mixed occupancy building
or portion of a mixed occupancy building need to clarify that any required
fire separations (floor assemblies, wall assemblies) are provided by others
in order for your 13R system to be adequate.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


New ICC Forum to Start

2011-08-30 Thread Bill Brooks
From the most recent ICC news:

ICC to Launch New Codes  Standards Discussion Forum - The International
Code Council will be launching the Codes  Standards Discussion Forum. This
new area of ICC's website will be centered around open discussion of the
International Codes and standards, allowing industry professionals to share
their ideas and knowledge with one another.

Seems like this will be the place to discuss the application of 13/13R and
other IBC issues.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Assembly area in R occupancy (IBC approach)

2011-08-30 Thread Bill Brooks
If the BUILDING is Use Group R and meets the story requirement, 13R is OK.
If the BUILDING is mixed use and occupancy, either separated or
non-separated, then use 13.

It would be up to the design professional to use the accessory and
incidental rules or other exceptions to classify the building.

Is it really this simple?

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, August 29, 2011 3:28 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: Assembly area in R occupancy

I am looking at an R-2 building (dormitory) with an A-2 (commons/kitchen) on
the first floor. The A-2 is over 750 sq feet (so not incidental). As far as
I can tell, this means that in order to use an NFPA 13R system in the
building, the A and R areas must have a 2 hour separation (since the
building is NOT sprinkled to 903.3.1.1)

Is this the way that everyone else sees it? I am double checking because I
consistently see architectural code sheets that list an A occupancy on the
first floor with a 1 hour separation from the R occupancies and they call
for a 13R system.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Water storage/NFPA 13 Proposal

2011-08-11 Thread Bill Brooks
I see four possible calculation approaches for the sprinkler demand part of
tank sizing:

1. Minimum Density x Tabular Design Area x Time
2. Minimum Density x Actual Design Area (developed using the 1.2 rule) x
Time
3. Hydraulically Calculated Demand (Demand Calc) x Time
4. Hydraulically Calculated Demand (Supply Calc) x Time

I intend to submit a Comment to clarify this.

#1 is the easiest for everyone, the others require the sprinkler system to
be fully designed before the tank size can be confirmed.  It's also evident
that all of the methods other than #4 will mean draining the tank in less
than the required time duration.

Then of course is how to decide whether to use 60 minutes or 90 minutes or
something in between for OH.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mark Sornsin
Sent: Tuesday, August 09, 2011 7:32 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage/NFPA 13 Proposal

I concur with Craig. 

It seems the proposal was written to clarify for AHJs that one needs NOT run
a separate calculation for sprinklers closest to the source simply to
identify maximum flows (and therefore maximum supply requirements). The
remote area calculation(s) is 'good enough'.  I do not think the proposal is
suggesting you can calc a tank based merely on 'density x area x duration =
volume'. The procedures in Chapters 11 through 22 for the required duration
as specified in Chapter 11, Chapter 12 and through Chapter 21 do not allow
you to omit overages within the design area.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

But we all know that a .15 gpm/sf over 1500 gpm doesn't calc out to exactly
225 gpm of flow and we know that most fires are controlled by 3 or less
sprinklers.  So if someone wants to cut it that close, go for it.  

Related to the question of whether to include hose stream or not, what's
interesting is that in other areas of 13, it is clearly spelled out that the
demand is to include both hose and sprinklers.

But in the NFSA response it's talking about not considering the excess flow
that is typical of sprinklers closer to the riser which are OUTSIDE of the
remote area.  It is NOT saying anything about factoring the imbalance or
overage for the remote area sprinklers.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:41 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote

RE: Water storage/NFPA 13 Proposal

2011-08-11 Thread Bill Brooks
Excuse my inability to read.

Bill Brooks


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, August 11, 2011 8:42 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage/NFPA 13 Proposal

There's no decision to make on whether to use 60 or 90 minutes.  The
Standard is clear on how that decision is to be made.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, August 11, 2011 8:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage/NFPA 13 Proposal

I see four possible calculation approaches for the sprinkler demand part of
tank sizing:

1. Minimum Density x Tabular Design Area x Time
2. Minimum Density x Actual Design Area (developed using the 1.2 rule) x
Time
3. Hydraulically Calculated Demand (Demand Calc) x Time
4. Hydraulically Calculated Demand (Supply Calc) x Time

I intend to submit a Comment to clarify this.

#1 is the easiest for everyone, the others require the sprinkler system to
be fully designed before the tank size can be confirmed.  It's also evident
that all of the methods other than #4 will mean draining the tank in less
than the required time duration.

Then of course is how to decide whether to use 60 minutes or 90 minutes or
something in between for OH.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mark Sornsin
Sent: Tuesday, August 09, 2011 7:32 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage/NFPA 13 Proposal

I concur with Craig. 

It seems the proposal was written to clarify for AHJs that one needs NOT run
a separate calculation for sprinklers closest to the source simply to
identify maximum flows (and therefore maximum supply requirements). The
remote area calculation(s) is 'good enough'.  I do not think the proposal is
suggesting you can calc a tank based merely on 'density x area x duration =
volume'. The procedures in Chapters 11 through 22 for the required duration
as specified in Chapter 11, Chapter 12 and through Chapter 21 do not allow
you to omit overages within the design area.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

But we all know that a .15 gpm/sf over 1500 gpm doesn't calc out to exactly
225 gpm of flow and we know that most fires are controlled by 3 or less
sprinklers.  So if someone wants to cut it that close, go for it.  

Related to the question of whether to include hose stream or not, what's
interesting is that in other areas of 13, it is clearly spelled out that the
demand is to include both hose and sprinklers.

But in the NFSA response it's talking about not considering the excess flow
that is typical of sprinklers closer to the riser which are OUTSIDE of the
remote area.  It is NOT saying anything about factoring the imbalance or
overage for the remote area sprinklers.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:41 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct

RE: Water storage

2011-08-09 Thread Bill Brooks
13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word

RE: Water storage

2011-08-09 Thread Bill Brooks
Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams

Seismic Bracing - Clean Agent

2011-08-08 Thread Bill Brooks
Perhaps a bit off the reservation here but does anyone out there have some
reason for the lack of clean agent system seismic bracing requirements?
Empty piping? Bracing already factored into piping design per ???

Feel free to send me to another listserv if one exists for special hazard
systems.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Seismic Bracing - Clean Agent

2011-08-08 Thread Bill Brooks
I saw that reference to ASME as well and made similar assumptions as you
made.  Yet it would mean a shop drawing review by the AHJ or the design
engineer would bring in all those ASME calculations.  But you'll note the
Working Plans section does not have any requirement for submission of those
ASME calculations to substantiate the hangar placement and attachments.

I've submitted this to NFPA for some feedback also.  I'll post their
response for list information.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, August 08, 2011 2:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Seismic Bracing - Clean Agent

If you're referring to NFPA 2001,  it references ASME B31.1 for direction on
support and bracing.  Yes, these systems are normally supported differently
than a wet pipe sprinkler system because the forces exerted upon the system
at discharge are far greater than a sprinkler system.  ASME B31.1 gets into
greater detail of hanging and bracing and refers back to ASCE 07 for systems
installed in seismically active areas.  So if a sprinkler system would
require EQ bracing, a clean agent system would as well.  One difference
being that the CA system support components may also be able to be counted
towards EQ bracing requirements when designed to the higher requirements.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Monday, August 08, 2011 1:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Seismic Bracing - Clean Agent

Perhaps a bit off the reservation here but does anyone out there have some
reason for the lack of clean agent system seismic bracing requirements?
Empty piping? Bracing already factored into piping design per ???

Feel free to send me to another listserv if one exists for special hazard
systems.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: How much discharge from a 2 system drain

2011-08-02 Thread Bill Brooks
I'd guess in the 350 to 400 gpm range if your main drain was attached
directly to the riser off a tee then 2 angle valve then drop to floor.
This is about 70 equivalent ft in length.With 100 psi at the riser you'd
see a loss of 85 psi between the riser and the main drain outlet leaving
around 15 psi at the outlet of the 2 pipe.  Since a 2 pipe has
approximately 17 times the area of a 1/2 sprinkler I'd multiply 22 gpm
times 17 to get 374 gpm.

Purely seat of the pants but old seat in pants.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 02, 2011 3:02 PM
To: sprinklerforum@firesprinkler.org
Subject: How much discharge from a 2 system drain

Plumbing engineer is asking how much flow could come from a 2 main drain at
the riser.  They are sizing floor sinks to capture the discharge.  No we're
not discharging it outside like usual.  This isn't a usual client.

System pressures from the pump are around 200psi static and 180 psi
residual.  That's a whole other issue.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Domestic Demand

2011-07-19 Thread Bill Brooks
Normally the engineer is supposed to consider this and incorporate some sort
of instructions with the bid package.  In my opinion, domestic demand should
ALWAYS be considered but many times does not change the outcome.  If you are
only the sprinkler designer how are you supposed to chase down all these
other subs in order to find out how much water they are using?  It's not the
sprinkler designer's job to guess.  For example, a military barracks job
with multiple buildings in proximity - hundreds of showers at the same time.
Perhaps a bottling plant with constant flow.  Lawn irrigation systems also.
I think that self shut off flows (toilet flush) can be ignored, but others
should be considered.  The plumbing engineer can (and should) provide a
number for these based on Hunter's curve or some other engineering method.  

Water tank make-up would be one of the flows to consider.

Probably a good practice on every job to send an early RFI and ask about all
these domestic flows.  Share the problem with others.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 9:12 AM
To: sprinklerforum@firesprinkler.org
Subject: Domestic Demand

I'm working on an Administration Building that has some really strange
underground  plumbing configurations with relationship to the sprinkler
riser and it got me to thinking about domestic allowance in calculations.
I'm looking for some information that says I don't need to include things
like chilled water, water tank make-up, etc. in the hydraulic calculations.
I can't remember a situation where I've ever included things like these in
my calculations but like I said earlier the incoming water supply has some
strange requirements that got me thinking. I know 11.1.4.3 says the minimum
water supply requirement shall be for the sprinklers and hose stream, is
this enough to hang my hat on?
 
Brian Harris, CET
First Defense Fire Protection
11957 Ramah Church Road
Huntersville, NC 28078
Phone: 704.948.3506
Fax: 704.948.3507
 




===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Domestic Demand

2011-07-19 Thread Bill Brooks
Interesting that the 2007 language (which was unenforceable) has been
eliminated in favor of the current 23.1.2 (which now could leave someone
open to liability).  I missed that.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Domestic Demand

Roland-
I don't see anything in chapter 23 that talks about including domestic in
the calc's, what am I missing?  


Brian Harris, CET
FDFP Inc.
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, July 19, 2011 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Domestic Demand

11.1.4.3 does not address domestic so you can't hang your hat on it.   
It's chap 23.

Roland

On Jul 19, 2011, at 6:11 AM, Brian Harris wrote:

 I'm working on an Administration Building that has some really strange 
 underground  plumbing configurations with relationship to the 
 sprinkler riser and it got me to thinking about domestic allowance in 
 calculations.
 I'm looking for some information that says I don't need to include 
 things like chilled water, water tank make-up, etc. in the hydraulic 
 calculations.
 I can't remember a situation where I've ever included things like 
 these in my calculations but like I said earlier the incoming water 
 supply has some strange requirements that got me thinking. I know 
 11.1.4.3 says the minimum water supply requirement shall be for the 
 sprinklers and hose stream, is this enough to hang my hat on?

 Brian Harris, CET
 First Defense Fire Protection
 11957 Ramah Church Road
 Huntersville, NC 28078
 Phone: 704.948.3506
 Fax: 704.948.3507





 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/ ===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Domestic Demand

2011-07-19 Thread Bill Brooks
I believe the 2007, 23.2.1.2 is unenforceable.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 10:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Domestic Demand

Bill-
What language would that be in the 07 edition? 


Brian Harris, CET
FDFP Inc.
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, July 19, 2011 10:33 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Domestic Demand

Interesting that the 2007 language (which was unenforceable) has been
eliminated in favor of the current 23.1.2 (which now could leave someone
open to liability).  I missed that.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Tuesday, July 19, 2011 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Domestic Demand

Roland-
I don't see anything in chapter 23 that talks about including domestic in
the calc's, what am I missing?  


Brian Harris, CET
FDFP Inc.
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, July 19, 2011 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Domestic Demand

11.1.4.3 does not address domestic so you can't hang your hat on it.   
It's chap 23.

Roland

On Jul 19, 2011, at 6:11 AM, Brian Harris wrote:

 I'm working on an Administration Building that has some really strange 
 underground  plumbing configurations with relationship to the 
 sprinkler riser and it got me to thinking about domestic allowance in 
 calculations.
 I'm looking for some information that says I don't need to include 
 things like chilled water, water tank make-up, etc. in the hydraulic 
 calculations.
 I can't remember a situation where I've ever included things like 
 these in my calculations but like I said earlier the incoming water 
 supply has some strange requirements that got me thinking. I know
 11.1.4.3 says the minimum water supply requirement shall be for the 
 sprinklers and hose stream, is this enough to hang my hat on?

 Brian Harris, CET
 First Defense Fire Protection
 11957 Ramah Church Road
 Huntersville, NC 28078
 Phone: 704.948.3506
 Fax: 704.948.3507





 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/ ===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17920)
http://www.pctools.com/
===





===
Email scanned by PC Tools

RE: Transition from Outside to Inside

2011-07-13 Thread Bill Brooks
Of course the Annex is not the body as the TC already knows, and of course
this is a pretty minor point, but fixing this, even as a change to the
Annex, is not that complex.  And why, if this is how the TC rationalizes
their opinion, would they address this topic in relation to location of the
piping with respect to the foundation?   I generally use the one joint
rule which would limit the amount of underground piping to less than one
length and thereby limiting the height of the flange above the floor (just
as is shown in A.10.6.5), but I have seen multiple pieces of ductile inside
as well.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, July 12, 2011 4:47 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Transition from Outside to Inside

I agree with Mark. Some folks (including the TC at the ROP meeting)  
seem to think it is acceptable based on 13:A.10.6.5 showing part of  
the underground pipe extending above the floor.  They seem to have  
ignored that the Figure is ductile so doesn't address plastic and seem  
to have forgotten that the listing for underground plastic pipe  
applies to it being underground.  As soon as it is exposed (whether in  
a trench or as a transition piece above the floor) it has to be  
acceptable as an above ground pipe. Needless to say, this issue will  
be addressed again at the ROC meeting.

Roland

On Jul 12, 2011, at 7:16 AM, Mark Sornsin wrote:

 Bill - I'm going to go on a limb a bit and suggest there is no  
 maximum height.

 There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the  
 transition piece (23.1.6.1.1). It is implied that underground pipe  
 is only underground. An aggressive AHJ or EOR may argue that the  
 flange must be located at the floor level - so no underground pipe  
 is above-ground and vice versa. I would suggest that it really only  
 matters when dealing with plastic underground transitioning to above- 
 ground pipe. No plastic pipe should be allowed above ground, so the  
 transition should start below grade. I always spec' ductile iron  
 into the building. This meets the intent of 23.1.6.1.1 as a  
 transition.  We normally shoot for the transition to the above- 
 ground pipe to occur at 6 to 12 inches above the floor, but there is  
 nothing in 13 that mandates any particular height.

 Mark A. Sornsin, PE| Fire Protection Engineer
 Ulteig Engineers, Inc.| Fargo, ND
 mark.sorn...@ulteig.com



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Transition from Outside to Inside

2011-07-12 Thread Bill Brooks
Something I thought I could find but couldn't.  What is the maximum height
for the floor flange to transition from the below ground pipe to the above
ground pipe?  (NFPA 13-2010, 6.3  23.1.6.1.1)  Ductile and plastic are not
listed in the Table 6.3.1.1.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Building trade off update

2011-06-23 Thread Bill Brooks
Important information revealed.  You'll probably get other feedback on this
but the V-B construction type matched up with the A-3 use would seem to
dictate a fully sprinklered 2-story building (IBC Table 503 and 504.2).  If
the architect is relying solely on 902.2.1.3 and 903.2.1 I believe he/she is
missing the Table 503 implications.  Of course this interpretation is based
on a reading of the IBC and no other building specifics.  To go to 2 stories
the automatic sprinkler system must be per NFPA 13 (504.2 and 903.3.1.1) and
here I'm not sure how a combustible attic can be excluded, even with
draftstops, but maybe there's something I've missed.

With V-A construction the 2-story would seem to be acceptable, but then you
would need to figure out if the attic is considered a story or not (see
STORY definition on IBC page 20).  If it is not a story then it could be
considered part of the 2nd floor which would need to be sprinklered per
903.2.1.  In either case you are led pretty much to a sprinklered attic, but
this last part is my interpretation of where things would go.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Thursday, June 23, 2011 12:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Building trade off update

Completely understand and as always appreciate your input my friend. 


V-B
Basement8,000
1st 8,500
2nd 8,000

Reviewing the referenced section 1018.1 and its exceptions. 

Thanks,

Rod

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Wednesday, June 22, 2011 9:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Building trade off update

See IBC Table 1018.1, Note c.  Also 

Also for our information, what is building construction type and what is
area per floor?

I'm trying to learn just as you are.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Wednesday, June 22, 2011 11:05 AM
To: sprinklerforum@firesprinkler.org
Subject: Building trade off update


I wanted to follow up and let everyone who helped me think through the
process know what happened. This was a new two story courthouse (A3) with a
combustible attic above the 2nd floor and a single (B) occupancy attached
adjacent on the ground floor.  IBC 2009. He was sprinklering the basement,
1st and 2nd but not the attic. We met with the Architect and and asked him
if he could educate us on his decision tree that allowed:


 1.   No sprinklers in the combustible attic that was draft stopped every
3,000 ft.
 2.   Install fire protection on the first and second floors (not  required
systems in the A3) to allow a reduction in fire rating of the corridor
walls, stairs, and the wall separating the courtroom A3 from the B
occupancy.
 3.  His logic for not mandating an increase of the design area on the 2nd
floor to 3,000 ft.

His answers were:


 1.  The IBC 2009 doesn't require sprinklers  except for the basement, so
NFPA 13 isn't applicable.
 2.  He stated that the IBC allows for reduction with partial systems. 901.2
exception
 3.  He believed that because partial systems are allowed and that because
the code didn't require a system in the attic that we wouldn't need to
increase our area on the 2nd floor even though the combustible attic above
was unsprinklered.

We took the advice of GC / Roland and others and listened and accepted what
he said. The tone of the meeting was very good and at the end of the day I
am glad he chose more sprinklers than required in lieu of more rating. I
personally don't agree with the lack of increase in area ( question #3) but
as it has been pointed out.. not my decision.

Thanks for all the input and help. We learn and move on.


Rod DiBona
Rapid Fire Protection

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum

RE: number of outlets on roof manifold

2011-06-15 Thread Bill Brooks
The objective is not to reach all areas of the roof because not all stairs
are required to have access to the roof (IBC 1009.13).  If all the stairs
had access to the roof, then IBC 905.4(5) would require a single hose
connection for each standpipe plus an additional connection for the
hydraulically most remote standpipe.  So that would be two connections for
the most remote and one for each of the others.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Wednesday, June 15, 2011 9:03 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: number of outlets on roof manifold

How many do you put at each landing?   The roof manifold is basically an
extension of the standpipe providing a hose connection on the roof.  So for
a single location, one outlet.  Depending on the size of the roof area you
may have more than one outlet on the roof in order to reach all areas of the
roof.  

The 2006-IFC 905.4(5) for Class I Standpipes states each standpipe shall be
provided with -- A -- hose connection located either on the roof or at the
highest landing of a stairway with stair access to the roof.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Wednesday, June 15, 2011 8:30 AM
To: sprinklerforum@firesprinkler.org
Subject: number of outlets on roof manifold

I could not find anything in either 14 or 25 that told me how many outlets
are needed on a roof manifold off a standpipe. Anybody know?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pump, Tank, 1000 ft suction line.....

2011-06-07 Thread Bill Brooks
You could represent the tank as a public supply with a static pressure equal
to the height of the water in the tank (problem is do you use full, half, or
empty elevation).  The residual pressure would be the at the pump suction
when you are flowing 1500 gpm.  I know it would look pretty weird showing
Static: 10 psi, Residual:  -45 psi, Flow: 1500 gpm @ pump suction, but this
is your reality with the 1000 ft of 6 suction piping.  Why would you even
send anything to an AHJ when you know the situation is not possible?
(rhetorical question)

I forgot, maybe the minimum suction pressure can't go below -14.7 so this
would mean considerably less flow than 1500.

Where are the academics when we need some hydraulic theory?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ralphy
Henderson
Sent: Tuesday, June 07, 2011 1:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pump, Tank, 1000 ft suction line.

No, I don't need a PC to do the calc but I'd like for hydra calc to show all
this w/o an additional set. Things like that tend to confuse the AHJ's -
especially hand written things. You would think a multi thousand dollar
program would be able to take the calc from a tank to the pump and to the
system in one report - but it looks like that's not the case.







--- On Tue, 6/7/11, George Church g...@rowesprinkler.com wrote:

From: George Church g...@rowesprinkler.com
Subject: RE: Pump, Tank, 1000 ft suction line.
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Date: Tuesday, June 7, 2011, 4:47 PM

Why not take a piece of paper, write down the length of the run, multiply it
by the FL/ft, and use a calculator to multiply the two and get the friction
loss?
Then correct for any dif in elevation by multiplying the dif x .433. 
It really isn't that hard and you really don't need a pc to run a simple
supply calc.

Ok, maybe I should say you SHOULDn'T need a pc


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ralphy
Henderson
Sent: Tuesday, June 07, 2011 12:29 PM
To: sprinklerforum@firesprinkler.org; b...@firebyknight.com
Subject: RE: Pump, Tank, 1000 ft suction line.

Bob, 

That's kind of what I was getting at. I'll probably just have to submit a
separate calc showing the 150% pump rating through the pump to the tank to
prove the losses are acceptable. Does anyone know if there is a way to do
this in a single calc in hydracalc? I can put in an additional water
'source' but then would have to enter in a static, res, and flow for the
tank to get it to run through the program and these numbers are unknown
(except for static).

Thanks,

RB


--- On Mon, 6/6/11, Bob b...@firebyknight.com wrote:

From: Bob b...@firebyknight.com
Subject: RE: Pump, Tank, 1000 ft suction line.
To: sprinklerforum@firesprinkler.org
Date: Monday, June 6, 2011, 11:05 PM

Ralph,
Looking at this I'm coming up with 20.3 psi loss in 1000' of pipe not
counting fittings and valves.
(4.52*1000.00^1.85)/(140^1.85*6.4^4.85) = .0203   .0203 * 1000 = 20.3. 6.4
is ID of 6 Tyton Joint Pipe DI.  Fittings and valves will increase your
losses.  At 1500 gpm you will have .43 psi / ft loss.  These numbers will
vary depending on pipe type and ID. As far as how to do it;  I think I would
simply run the numbers through the calculation back to the tank.  Or better
yet, if there are hydrants fed off of the tank have a flow test performed
and calc back to that point of connection.

Bob Knight, CET III
208-318-3057
www.firebyknight.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik
Sent: Monday, June 06, 2011 4:37 PM
To: sprinklerforum@firesprinkler.org; tm...@mfpdesign.com
Subject: Re: Pump, Tank, 1000 ft suction line.

Ralph -

My rough calcs say about 16 psi loss at 100% flow and 34 psi loss at 150%
flow.
Unless this is an elevated tank, or your source is uphill from the pump,
this won't work.

At 06:32 PM 6/6/2011, you wrote:
at 1000 gpm, you are going to lose about 2 psi per 100' of 6 
ductile iron pipe.  At 1500 gpm, you are going to lose about 5 psi / 
100' of DI pipe.  You need to have enough elevation between the tank 
and pump to provide a positive pressure at the suction flange.

On 6/6/2011 3:28 PM, Ralphy Henderson wrote:
Hi All,

Can someone explain to me how one would go about calculating a fire 
pump being fed solely from a water storage tank but with a 6 x
1,000 ft suction line? I've calculated fire pumps off

RE: CC1/CC2 or COIN sprinklers

2011-06-06 Thread Bill Brooks
Do you have the 2009 IBC available?  You're installing a 13R system?  Would
sprinkler protection be necessary in the attic space?  If NFPA 13R and no
sprinklers in the attic, then 3,000 sq ft draftstopping is needed.  This
would definitely be the architect's job to show these in my opinion.  If no
draftstopping is in the job, then your sprinkler scope extends to the attic.
If you must use a specially listed head for this purpose and if this head
requires 1000 sq ft draftstopping then it seems better to add the 3000 sq ft
draftstopping (or two units) and omit the sprinklers.

Have I interpreted this correctly, aside from any Marriott special
requirements?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: Monday, June 06, 2011 1:04 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: CC1/CC2 or COIN sprinklers

Looking for some other forum experience here.  How have you been dealing 
with architects and GC's that state the IBC does not require draft stops 
in an attic, so they are not willing to put them in when the CC heads 
are req'd and the CC heads require a draft curtain to be installed?

On 6/6/2011 9:23 AM, Matt Grise wrote:
 I agree. Just looked at that this morning. The handbook elaborates that
testing has found standard sprinks to be ineffective in short flat comb
concealed spaces.

 Matt Grisé PE*, LEED AP
 Sales Engineer
 Alliance Fire Protection
 130 w 9th Ave.
 North Kansas City, MO 64116

 *Licensed in KS  MO

 913.888.0647 ph
 913.888.0618 f
 913.927.0222 cell
 www. AFPsprink.com


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
 Sent: Monday, June 06, 2011 11:22 AM
 To: 'sprinklerforum@firesprinkler.org'; 'tm...@mfpdesign.com'
 Subject: RE: CC1/CC2 or COIN sprinklers

 Yes.  See 8.15.1.6 (2007).

 Duane Johnson, PE
 Program Manager
 Division of the Fire Marshal (Support Contractor)
 Office of Research Services
 National Institutes of Health
 301-496-0487

 Protecting Science - One Sprinkler at a Time


 -Original Message-
 From: Travis Mack, SET [mailto:tm...@mfpdesign.com]
 Sent: Monday, June 06, 2011 12:08 PM
 To: sprinklerforum@firesprinkler.org
 Subject: CC1/CC2 or COIN sprinklers

 Trying to settle a discussion here.  When you have a flat concealed
 combustible space and36 of clearance, are the specially listed heads
 required?

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: building code tradeoff

2011-05-27 Thread Bill Brooks
Rod, I know your heart is in the right place but you need to consult with a
codes professional on this and you may have to pay for these services.  I
would think your responsibility is to implement the scope you are given,
unless you intend to apply (or supply) and engineering seal on your
drawings.  In that case you may share the liability of bad advice given by
others.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Thursday, May 26, 2011 8:08 PM
To: sprinklerforum@firesprinkler.org
Subject: building code tradeoff

We have a project where the architect has stated the following:


1.  We have installed draftstops in the attic space to subdivide the
space into areas less than 3000 sf.


2.  We are installing the fire protection system in the basement
according to 903.2.11.1.


3.  We are installing fire protection on the first and second floors to
allow a reduction in fire rating of the corridor walls, stairs, and the wall
separating the courtroom A3 from the B occupancy.


4.  We are installing the draftstops in the attic space and not
accepting the reduction but utilitzing the exception to 901.2.



5.  The architect has stated that only the basement is required to be
sprinklered.

This is a new courthouse. This is an architect that we have done work with
and he is sharp but I don't see read the IBC the same way. First we were
questioning not sprinklering the combustible attic. We don't have the water
available to do a dry system in that attic without a fire pump. I don't
think the reductions can be taken on first and second floor unless the
entire building is sprinklered per NFPA 13. Can he subdivide with draftstops
and then take the rating reductions on the first and second floor? I don't
think so but even if I am wrong and this can be done, wouldn't we still have
to increase our area on the second floor to 3,000ft? If so we would need the
pump anyway. Thanks for your input.

Rod DiBona
Rapid Fire






___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


  1   2   3   >