RE: Nipple Extenders

2008-05-09 Thread Mike Brown (TECH- GVL)

United Brass makes a 1/2 by 1/2 male by female and a 3/4 x 3/4 male by 
female extender.  These can be used to extend a drop that is cut too short.  
AFSA in the past had a BEST PRACTICE written about the use of these.  There 
is some argument that these should not be used but they can be helpful.  There 
is also a company that makes a cast iron version of the same thing and they are 
a little longer than the brass ones.  I was always more comfortable using the 
brass extender nipples.  You can contact AFSA or go on their website to see if 
you can find the article in the archives'.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski
Sent: Thursday, May 08, 2008 5:21 PM
To: sprinklerforum@firesprinkler.org
Subject: Nipple Extenders

Quick (I hope) question.



I don't recall seeing this thread before. Are ½ x 1  male female nipple
extenders allowed to be used at the sprinkler/reducer coupling interface
when you have cut the drop a smidgen too short and can't get back above the
hard ceiling to pull it out?



 Mike Wisneski





 3898 Leeds Avenue

 North Charleston, SC 29405

 Phone: 843-767-3080

 Cell: 843-200-5710

 Fax: 843-767-5596

 Email : [EMAIL PROTECTED]

 Web   :
file:///C:\Documents%20and%20Settings\User\Application%20Data\Microsoft\Sig
natures\www.pyebarkerfiresafety.com www.pyebarkerfiresafety.com



This e-mail, including attachments, may include  confidential and /or
proprietary information, and may be used only by the person or entity to
which it is addressed. If the reader of this e-mail is not the intended
recipient or his or her authorized agent, the reader is hereby notified that
any dissemination, distribution or copying of this e-mail is prohibited. If
you have received this e-mail in error, please notify the sender by replying
to this message and delete this e-mail immediately



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Return Bends

2008-05-08 Thread Mike Brown (TECH- GVL)
As I remember the return bend was to help insure that creeping crud and 
corrosion does not build up on the orifice inlet of the sprinkler and cause 
problems with the operation of the sprinkler.  Or maybe I am just getting brain 
hiccups.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Thursday, May 08, 2008 9:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Return Bends

I know it doesn't seem right. But is it achieving its intent? Return bends
are used to prevent scale and other sediments being trapped at the head. To
some extent, at least except from the individual branchline, won't this be
achieved?

Tony

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: May 8, 2008 5:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Return Bends

what is being proposed to you is a line on a riser nipple off of the main
NOT return bends.  The return bend is there for a reason and what is being
proposed to you does not serve the purpose.  The suggestion should be
rejected.

Garth

- Original Message -
From: A.P.Silva [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Wednesday, May 07, 2008 11:08 PM
Subject: Return Bends


 I have a situation, dry system running in heated space below the attic in
 part of the building. In other parts, within the attic space. Where it is
 running in the heated area, sprinklers are pendent type. So the need for
dry
 pendents or return bends. The contractor doesn't want to install
individual
 return bends for each pendent head (for cost reasons). Instead he is
 proposing to make the entire branchline as the return bend. The branchline
 to have a riser at the connection to the main. Then from the branchline
drop
 down directly to each pendent head. Any problems?

 Tony

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Mike Brown (TECH- GVL)
My point is that the NFPA 13D Committee should provide guidelines to follow in 
these situations.  I do not care if they say calculate the room to light hazard 
as long as they put it in writing. But the way it is now, it is just what ever 
the contractor or engineer (designer) can get the AHJ to go along with.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matsuda, Richard
Sent: Tuesday, May 06, 2008 5:08 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Residential Sprinklers and Beam Obstructions

  I love these discussions cause I get to hear about the problems that
the contractors have in designing these systems. Guess what...we (the
AHJ) have the same problems trying to approve them.

I remembered a similar discussion saying something about not allowing
them to build something that you can't protect...I think it was a boat
storage rack or something about ESFR sprinklers. The problem with these
houses is that the architect, builder, and home owner have conspired to
build them and now we have to figure out how to protect them. I guess I
could tell them to rip it all out and make a smooth flat ceiling, but I
don't think that would be acceptable to our administration.

So what do we do? My simplistic answer is that if it looks like an
over-kill design with 10 heads in a 20 x 20-foot room, then it probably
is a waste of money. If one head can protect the room with a smooth flat
ceiling, then maybe four or five heads should be reasonable with beam
pockets. Depends on the size and occupancy of the room, beam locations,
depth, ceiling height, type of sprinklers used, and other
variables...but there is a  reasonable answer to it. The difficulty is
deciding what's reasonable...and no single solution will fit all
situations.

rick matsuda
city of dallas, bldg insp dept

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Tuesday, May 06, 2008 11:52 AM
To: sprinklerforum@firesprinkler.org
Subject: Residential Sprinklers and Beam Obstructions

I'm working on a home (13D) that has several rooms with the ceiling
broken
up by beam pockets.  These vary in width from 2'8 to 3'3 o.c. with
the
beams being 6 deep.  Concealed residential sprinklers are being used.
In
one room, which is 224 sf, if I place a sprinkler in every pocket like I
think I should, there will be 13 sprinklers.  This averages out to 17 sf
per
head.  Another room is 375 sf and will require 10 sprinklers.  This
averages
at 37.5 per head.  In rooms of this size do I really need a sprinkler in
every pocket?  Can a sprinkler be placed in every other pocket and be
acceptable?  Has anyone else found a better way to protect rooms like
this?
Any and all suggestions will help.

Thanks,

Bob Knight, CET
(208) 318-3057
[EMAIL PROTECTED]
www.firebyknight.com
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Mike Brown (TECH- GVL)
The NFPA 13D Committee in their wisdom (or as some people have suggested lack 
thereof) put in the 2007 Edition Paragraph 8.1.3.1.2

Where construction features or other special conditions exist that are outside 
the scope of sprinkler listings, listed sprinklers shall be permitted to be 
installed beyond their listing limitations.


I hope that you and the AHJ have good insurance or a lot of money.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, May 06, 2008 2:03 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Residential Sprinklers and Beam Obstructions

Bob:

We run into this all the time. First question are the beams structural? If
the beams are decorative only drill the beams use your concealed heads and
space as normal. While the beam rules for TYCO are ok, they have a lot of
situations where you would have to tell the Arch. how to layout the beams
before hand.(Like that's ever going to happen!) If you read the white paper
for slope Beam ceilings exceeding 8/12 you'll see that the concealed
sprinklers responded slightly better when in the beams than in the pockets.
If this is true on a steep slope ceiling it should be reasonable to apply it
to flat beam ceilings. (With heads in the beams less than 12 below the
actual flat ceiling, we usually use the flows for 8/12 slope to offset any
delay for the lower position of the heads,) All our AHJ's are OK with this.

If your beams are structural, good luck getting the Arch. or Structural Eng.
to let you put a 21/2 hole vertically thru a structural member. Then we
usually end up with heads in every pocket, because you can't center a head
and still get far enough away from the beams to spray under them.

Good Luck!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: Bob Knight [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Tuesday, May 06, 2008 10:51 AM
Subject: Residential Sprinklers and Beam Obstructions


 I'm working on a home (13D) that has several rooms with the ceiling broken
 up by beam pockets.  These vary in width from 2'8 to 3'3 o.c. with the
 beams being 6 deep.  Concealed residential sprinklers are being used.  In
 one room, which is 224 sf, if I place a sprinkler in every pocket like I
 think I should, there will be 13 sprinklers.  This averages out to 17 sf
 per
 head.  Another room is 375 sf and will require 10 sprinklers.  This
 averages
 at 37.5 per head.  In rooms of this size do I really need a sprinkler in
 every pocket?  Can a sprinkler be placed in every other pocket and be
 acceptable?  Has anyone else found a better way to protect rooms like
 this?
 Any and all suggestions will help.

 Thanks,

 Bob Knight, CET
 (208) 318-3057
 [EMAIL PROTECTED]
 www.firebyknight.com


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: What is a Bucket Test?

2008-04-24 Thread Mike Brown (TECH- GVL)
Actually, in several counties around Atlanta, the test was also required for 
garden style apartments up to four stories.  You would be surprised that, at 
least in the beginning, a number of projects that had full blown hydraulic 
calculations failed when the bucket test showed them to be incorrect.  Many 
times the main culprit was a water test supplied by the water company that was 
faulty or not up to date.  Which brings me to my point that I have made over 
the years, the design of sprinkler systems really involves four major 
decisions by the design engineer and the rest is mostly a layout of a system 
within the rules of the codes.

First Engineering Decision: What is the hazard and what densities are 
required.  The project must be classified as per the fire risk. What are you 
protecting and how much water will it require to achieve the fire protection 
objective.

Second Engineering Decision:  What is the water supply and has there been a 
detailed analysis and testing of the water supply?  Generally, engineers and 
others rely on water tests provide by others and sometimes incorrect and out of 
date. Often very little time is devoted by the engineer to insure that an 
adequate water supply at the needed pressure is available.  This does not mean 
just throwing in a large fire pump just to be safe.

Third Engineering Decision:  Where is the remote area?  It is easy to just let 
the designer decide but the selection of the remote area can change the 
hydraulics dramatically.

Fourth Engineering Decision:  Coordination and review of the plans. The shop 
drawings and calculations may be checked and the coordination with the other 
trades on the project.  Often, the engineer just passes these functions to a 
trainee or someone else within the engineering firm. In other cases the issue 
is just ignored.

Too often these decisions are not given the time and effort that they deserve.


Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Wednesday, April 23, 2008 8:08 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

Bucket test, IMHO, was to prove the shortcut calcs allowed under 13D
worked. 13R calcs are done to the same level of care as #13 calcs, so no
bucket test was needed.

In #13D done with shortcut calcs, makes sense and isn't a big deal-
especially when you consider the downside (fire death in sprinklered house).

But flowing 20 heads in a 13 system? Be careful what you ask for is right.

glc


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, April 10, 2008 12:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: What is a Bucket Test?

Chris,

This silly test tells you nothing that other tests don't already tell
you. It certainly doesn't tell you if your system will work or not
because it presumes that conditions at the moment of the bucket test
reflect the moment of the water availability test. Main drain tests
will tell you if pipe is collapsed or valves are shut. What needs to
be done (and I know this won't happen) is to get the water purveyors
to quit handing out old crap and calling it good today. Thanks for
setting me up for this mini-rant.

Ron Greenman
...at home


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: engineering decisions

2008-04-24 Thread Mike Brown (TECH- GVL)
Roland
This will get you going---As usual the engineer does not want to do anything 
but get paid.

 Just write in the spec:

[Sprinkler System as per NFPA 13 and all materials and design shall meet UL 
and FM Approvals.  Contractor shall meet all state and local codes.  Contractor 
shall determine the water supply and all drawings are schematic and the 
co-ordination and/or anything else required is to be the responsibility of the 
contractor.]

Have a good day!

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins
Sent: Thursday, April 24, 2008 10:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: engineering decisions

Mike: You need to update (that is reduce) your list.  First expand
item 2 to identify the engineer needs to determine IF The water
supply is adequate.  I've never understood how an AE team can provide
room for a pump and it's associated infrastructure if they don't know
one is needed until a subcontractor tells them.  Now break out the
chain saw. The Third item is definitely to be thrown out.  How can
the EOR identify where the remote area is unless they are drawing
lines and circles?  Keep cutting and throw out item 4.  The AHJ
blesses the plans and do you really want a third party slowing you
down for coordination? Although the engineering job assurance plan
has this one listed, it is a contractual thing can implement IF the
owner wants it but not a valid requirement.  The exception to this
statement are when BUILDINGS are designed on a performance basis that
requires specific sprinkler criteria (that can exceed 13).

Roland

On Apr 24, 2008, at 6:15 AM, Mike Brown (TECH- GVL) wrote:

 Actually, in several counties around Atlanta, the test was also
 required for garden style apartments up to four stories.  You would
 be surprised that, at least in the beginning, a number of projects
 that had full blown hydraulic calculations failed when the bucket
 test showed them to be incorrect.  Many times the main culprit was
 a water test supplied by the water company that was faulty or not
 up to date.  Which brings me to my point that I have made over the
 years, the design of sprinkler systems really involves four major
 decisions by the design engineer and the rest is mostly a layout of
 a system within the rules of the codes.

 First Engineering Decision: What is the hazard and what
 densities are required.  The project must be classified as per the
 fire risk. What are you protecting and how much water will it
 require to achieve the fire protection objective.

 Second Engineering Decision:  What is the water supply and has
 there been a detailed analysis and testing of the water supply?
 Generally, engineers and others rely on water tests provide by
 others and sometimes incorrect and out of date. Often very little
 time is devoted by the engineer to insure that an adequate water
 supply at the needed pressure is available.  This does not mean
 just throwing in a large fire pump just to be safe.

 Third Engineering Decision:  Where is the remote area?  It is easy
 to just let the designer decide but the selection of the remote
 area can change the hydraulics dramatically.

 Fourth Engineering Decision:  Coordination and review of the plans.
 The shop drawings and calculations may be checked and the
 coordination with the other trades on the project.  Often, the
 engineer just passes these functions to a trainee or someone else
 within the engineering firm. In other cases the issue is just ignored.

 Too often these decisions are not given the time and effort that
 they deserve.


 Michael L. Brown
 Manager of Technical Services
 The Reliable Automatic Sprinkler Company, Inc.'
 [EMAIL PROTECTED]
 www.reliablesprinkler.com
 (864) 843-5228

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: engineering decisions

2008-04-24 Thread Mike Brown (TECH- GVL)
Joe
I realize that but I have seen hundreds of specifications where the engineer 
specs it that way requiring both UL and FM Approval.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Thursday, April 24, 2008 12:33 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: engineering decisions

Just remember, it's not possible to meet all FM requirements without FM
being involved. It can't be done with just a copy of FM Data Sheets.

Joe


Mike Brown (TECH- GVL) wrote:
 Roland
 This will get you going---As usual the engineer does not want to do anything 
 but get paid.

  Just write in the spec:

 [Sprinkler System as per NFPA 13 and all materials and design shall meet UL 
 and FM Approvals.  Contractor shall meet all state and local codes.  
 Contractor shall determine the water supply and all drawings are schematic 
 and the co-ordination and/or anything else required is to be the 
 responsibility of the contractor.]

 Have a good day!

 Michael L. Brown
 Manager of Technical Services
 The Reliable Automatic Sprinkler Company, Inc.'
 [EMAIL PROTECTED]
 www.reliablesprinkler.com
 (864) 843-5228

 -Original Message-
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins
 Sent: Thursday, April 24, 2008 10:59 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: engineering decisions

 Mike: You need to update (that is reduce) your list.  First expand
 item 2 to identify the engineer needs to determine IF The water
 supply is adequate.  I've never understood how an AE team can provide
 room for a pump and it's associated infrastructure if they don't know
 one is needed until a subcontractor tells them.  Now break out the
 chain saw. The Third item is definitely to be thrown out.  How can
 the EOR identify where the remote area is unless they are drawing
 lines and circles?  Keep cutting and throw out item 4.  The AHJ
 blesses the plans and do you really want a third party slowing you
 down for coordination? Although the engineering job assurance plan
 has this one listed, it is a contractual thing can implement IF the
 owner wants it but not a valid requirement.  The exception to this
 statement are when BUILDINGS are designed on a performance basis that
 requires specific sprinkler criteria (that can exceed 13).

 Roland

 On Apr 24, 2008, at 6:15 AM, Mike Brown (TECH- GVL) wrote:


 Actually, in several counties around Atlanta, the test was also
 required for garden style apartments up to four stories.  You would
 be surprised that, at least in the beginning, a number of projects
 that had full blown hydraulic calculations failed when the bucket
 test showed them to be incorrect.  Many times the main culprit was
 a water test supplied by the water company that was faulty or not
 up to date.  Which brings me to my point that I have made over the
 years, the design of sprinkler systems really involves four major
 decisions by the design engineer and the rest is mostly a layout of
 a system within the rules of the codes.

 First Engineering Decision: What is the hazard and what
 densities are required.  The project must be classified as per the
 fire risk. What are you protecting and how much water will it
 require to achieve the fire protection objective.

 Second Engineering Decision:  What is the water supply and has
 there been a detailed analysis and testing of the water supply?
 Generally, engineers and others rely on water tests provide by
 others and sometimes incorrect and out of date. Often very little
 time is devoted by the engineer to insure that an adequate water
 supply at the needed pressure is available.  This does not mean
 just throwing in a large fire pump just to be safe.

 Third Engineering Decision:  Where is the remote area?  It is easy
 to just let the designer decide but the selection of the remote
 area can change the hydraulics dramatically.

 Fourth Engineering Decision:  Coordination and review of the plans.
 The shop drawings and calculations may be checked and the
 coordination with the other trades on the project.  Often, the
 engineer just passes these functions to a trainee or someone else
 within the engineering firm. In other cases the issue is just ignored.

 Too often these decisions are not given the time and effort that
 they deserve.


 Michael L. Brown
 Manager of Technical Services
 The Reliable Automatic Sprinkler Company, Inc.'
 [EMAIL PROTECTED]
 www.reliablesprinkler.com
 (864) 843-5228


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field

RE: What is a Bucket Test? (TIA Needed)

2008-04-15 Thread Mike Brown (TECH- GVL)
John
You start with a set of approved plans with the hydraulic calculations and a 
permit.  There would be various stages of inspection depending on the local 
fire marshal and the Bucket test would be before cover up of the pipe and 
fittings. If there have been changes made to the piping,they should show up on 
an as-built drawing (as-built drawings are difficult to get correct even with 
commercial systems).  The bucket test would at least insure that the remote 
sprinklers flow the minimum water as per the hydraulic calculations.


Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Monday, April 14, 2008 4:03 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test? (TIA Needed)

Mike,

In addition to revised plans and hydraulic calculations where the job
wasn't installed to the original plan ?

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown (TECH- GVL)
Sent: Monday, April 14, 2008 3:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test? (TIA Needed)

I agree with Thom in that, as we are getting closer to mandated fire
sprinklers in single family homes, the potential for a large number of
new contractors, plumbers, and assorted others (some of whom may well be
trunk slammers) will be jumping on the bandwagon.  As I remember when we
were getting a licensing law in Georgia, we had to exempt single family
homes in order to get any kind of law.  In some states there is still no
law at all. (New York State for example has no licensing law.) This
influx of new sprinkler installers may not be well versed sprinkler
installation.  A Put the Water in the Bucket test might well be a good
control measure to protect the potential home owner as well as
protecting the image of our industry.  I would think that a test like
this might be included in the next edition of NFPA 13D.

At least, when I see some of the questions that I get from some
sprinkler contractors and a lot of engineers, a field test like this
could give us some degree of quality control. That would be a good
thing.

Something to consider.

Michael L. Brown, P.L.L.  (Peon Low Life) Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, April 14, 2008 1:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: What is a Bucket Test? (TIA Needed)

This TEST was a conditional method when 13D was new. I have not seen a
bucket test that failed, when required, in the last 15 years.
AHJ's are more savvy, Contractors are more cautious, and know that the
field guys will be adding ells. Some just add extra ells in the calc's
and others don't use the full residual pressure as allowed in 13D. Maybe
the bucket test would be ok if hydraulic calc's are not required, but is
a waste of time and money for Qualified  Designers and layout Tech's,
Installers, and AHJ's.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 14, 2008 10:05 AM
Subject: RE: What is a Bucket Test? (TIA Needed)


 Perhaps it is time to incorporate a bucket test requirement and test
 method into 13D prior to the widespread installation of these systems
 based on an ICC code change.  If failures are widespread I think this
 is important enough for a TIA if there's any chance the ICC will
 reference a current edition of 13D.  The implications are huge if
 large numbers of 13D systems are expected to fail after being
 engineered and installed by qualified plumbers/sprinkler companies.

 Bill Brooks

 William N. Brooks, P.E.
 Brooks Fire Protection Engineering Inc.
 372 Wilett Drive
 Severna Park, MD 21146
 410-544-3620 Phone
 410-544-3032 FAX
 412-400-6528 Cell

  Original Message 
 Subject: RE: What is a Bucket Test?
 From: Tom Duross [EMAIL PROTECTED]
 Date: Mon, April 14, 2008 11:05 am
 To: sprinklerforum@firesprinkler.org

 Back in the late eighties and early nineties, virtually every D and R
 system we did or designed got a bucket test. I still have my graduated

 buckets and pendent tubes we used. There's a couple of towns here in
 MA that still require them. I don't remember being waived on an R
 multi-family system back when they were all following what the Cobb
 Cty. Chief advised. I seem to remember every one of these systems were

 being bucket tested. We never failed a single one but I know some did.

 Tom Duross
 Go Red Sox
 :)

 I

RE: What is a Bucket Test?

2008-04-09 Thread Mike Brown (TECH- GVL)
I am sure if you contact the Cobb County Georgia Fire Department they will tell 
you about a lot of failures particularly when they first started.  The local 
contractors know about the test and check it themselves before they call for an 
inspection.  You guys are very diligent about your calculations etc. but there 
is a big world of contractors and engineers that are not part of this group who 
are not as versed in design as you may be.  It is a very simple test and it 
empirically proves that the system design is correct.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jamie Seidl
Sent: Wednesday, April 09, 2008 3:17 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

I've only had one that failed.  It turned out that the plumber had installed a 
1 line into the building from the meter (2 thru the slab) when we needed a 2 
line from the meter.  That is the reason for the bucket test, make sure the 
calc's work.  We could all argue quite correctly that it's not necessary but I 
am very comfortable with doing these test.  It just verifies that the whole 
system (at least the remote area) was installed correctly and will perform as 
intended.

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, April 09, 2008 3:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

Now that we have some what and where how about the why?

Brian's problem would have been discovered by looking at the gauge or main
drain, a bucket test wasn't really necessary.  Is there some problem with
hydraulic calcs?  How many actually fail?

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
Waverly, MN 55390

Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jamie Seidl
Sent: Wednesday, April 09, 2008 1:23 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

Quite a few in the North Carolina and Georgia area.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Wednesday, April 09, 2008 2:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

This is the first time I've heard it being done for 13R. 13D, yes. But not
13R. Are there other jurisdictions requiring a bucket test for 13R?

Tony

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: April 9, 2008 12:01 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

A bucket test / barrel test is when you remove a head(s) in the remote area
and fill up a bucket/barrel to see if it is flowing the gpm the is called
for in the calc's. In our case with the density and heads we are using that
would be 20 gpm, we are getting around 15 gpm.


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, April 09, 2008 1:50 PM
To: sprinklerforum@firesprinkler.org
Subject: What is a Bucket Test?

Perhaps a dumb question, but what is a bucket test and is it conducted the
same way in every jurisdiction?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

 Original Message 
Subject: Failed Bucket Test
From: Brian Harris [EMAIL PROTECTED]
Date: Mon, April 07, 2008 2:30 pm
To: sprinklerforum@firesprinkler.org

Fellow forum people:
I have a situation where we have designed and installed a 13R system, it is
completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns out
that a test taken now with the failed test shows a 25% drop in static 
residual pressures, hence the failed test. Of course the owner is looking to
us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a
few different things but with that big of a pressure loss there's really not
much we can do. I don't feel it's our liability at this point since we went
off the city's water flow test and per the calc's we were good, any
thoughts?


Regards,


http://www.firstdefensefire.com/








E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the 

RE: What is a Bucket Test?

2008-04-09 Thread Mike Brown (TECH- GVL)
You use the orifice size of the sprinklers that you are testing.  You install 
full port ball valve in a drain pipe from each of the sprinklers you are 
testing with the correct orifice. If you contact Cobb County, GA you can get 
their procedures if you are interested.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: Wednesday, April 09, 2008 3:47 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: What is a Bucket Test?

What kind of variance in calcs from actual bucket test results are
considered acceptable? I'm just curious since taking out the head and
flowing straight from a 1/2 threaded outlet vs. flowing a 7/16 orifice
(like a 4.2k sprinkler w/ element removed) could possibly work in your favor
to a small degree but could also work against you depending on what k-factor
of sprinkler you used.


In a 13R bucket test do you actually remove more than one sprinkler and flow
up to four? Or is it always just one? Seems like a source calc w/ one
sprinkler flowing would make more sense if you're only required to bucket
test one sprinkler...

-B-




On 4/9/08, Todd Williams - FPDC [EMAIL PROTECTED] wrote:

 If you have a really bad water supply, instead of a pitot you use a
 5-gallon bucket and a stop watch. 8-)


 At 02:19 PM 4/9/2008, you wrote:

  This is the first time I've heard it being done for 13R. 13D, yes. But
  not
  13R. Are there other jurisdictions requiring a bucket test for 13R?
 
  Tony
 
  -Original Message-
  From: [EMAIL PROTECTED]
  [mailto:[EMAIL PROTECTED] On Behalf Of Brian
  Harris
  Sent: April 9, 2008 12:01 PM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: What is a Bucket Test?
 
  A bucket test / barrel test is when you remove a head(s) in the remote
  area
  and fill up a bucket/barrel to see if it is flowing the gpm the is
  called
  for in the calc's. In our case with the density and heads we are using
  that
  would be 20 gpm, we are getting around 15 gpm.
 
 
  Brian Harris
  FDFP INC.
 
  -Original Message-
  From: [EMAIL PROTECTED]
  [mailto:[EMAIL PROTECTED] On Behalf Of
  [EMAIL PROTECTED]
  Sent: Wednesday, April 09, 2008 1:50 PM
  To: sprinklerforum@firesprinkler.org
  Subject: What is a Bucket Test?
 
  Perhaps a dumb question, but what is a bucket test and is it conducted
  the
  same way in every jurisdiction?
 
  Bill Brooks
 
  William N. Brooks, P.E.
  Brooks Fire Protection Engineering Inc.
  372 Wilett Drive
  Severna Park, MD 21146
  410-544-3620 Phone
  410-544-3032 FAX
  412-400-6528 Cell
 
   Original Message 
  Subject: Failed Bucket Test
  From: Brian Harris [EMAIL PROTECTED]
  Date: Mon, April 07, 2008 2:30 pm
  To: sprinklerforum@firesprinkler.org
 
  Fellow forum people:
  I have a situation where we have designed and installed a 13R system, it
  is
  completely finished and wham-o we fail the bucket test! Our system was
  designed based on the flow test provided by the city fire dept., turns
  out
  that a test taken now with the failed test shows a 25% drop in static 
  residual pressures, hence the failed test. Of course the owner is
  looking to
  us to pull a magic rabbit out of our #$% , err I mean hat, we have tried
  a
  few different things but with that big of a pressure loss there's really
  not
  much we can do. I don't feel it's our liability at this point since we
  went
  off the city's water flow test and per the calc's we were good, any
  thoughts?
 
 
  Regards,
 
 
  http://www.firstdefensefire.com/
 
 
 
 
 
 
 
 
  E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
  5.09560 http://www.pctools.com/spyware-doctor/
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
  to:[EMAIL PROTECTED][EMAIL PROTECTED]
  (Put the word unsubscribe in the subject field)
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
  to:[EMAIL PROTECTED][EMAIL PROTECTED]
  (Put the word unsubscribe in the subject field)
 
 
 
 
 
  E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
  5.09590 http://www.pctools.com/spyware-doctor/
 
 
 
 
 
  E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
  5.09590 http://www.pctools.com/spyware-doctor/
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
  to:[EMAIL PROTECTED][EMAIL PROTECTED]
  (Put the word unsubscribe in the subject 

RE: U.S. Fire Administration Policy on Residential Sprinklers

2008-03-31 Thread Mike Brown (TECH- GVL)
I guess I have stirred up enough discussion today but I am concerned about the 
use of control and suppression when residential sprinklers are not designed 
or tested to either control or suppress the fire.  In our desire to promote 
residential sprinklers some folks have in my opinion have over sold the 
capabilities of residential sprinklers in this area. Sure there are a lot of 
cases where if it catches the fire early it can control and suppress it but 
that is just a bonsus.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Monday, March 31, 2008 3:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: U.S. Fire Administration Policy on Residential Sprinklers

Hi Mike,

I was referring to smoke alarms which are required in all residential
dwellings pursuant to the building  residential codes and interestingly
by NFPA-13D (2007 NFPA-13D 4.7) in accordance with NFPA-72, as opposed
to sprinkler alarms and supervision which as you pointed out is not
required on 13D's.

Just wanted to make sure no confusion on that.

John Drucker

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown (TECH- GVL)
Sent: Monday, March 31, 2008 2:45 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: U.S. Fire Administration Policy on Residential Sprinklers

Just a little further information.  First alarms are not required on
NFPA 13D systems but that is for another day.

I have been in meetings with some of the advocates and installers where
control and suppression are thrown around frequently.  Additionally, one
individual that was advocating PreAction systems in NFPA 13D systems
stated as a reason the owner had ten million dollars of paintings in his
home and was worried about water damage.

Property Protection vs. Life Safety  ??

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Monday, March 31, 2008 1:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: U.S. Fire Administration Policy on Residential Sprinklers

It is infact as Mike says, then again the same can be said about
installing local smoke alarms versus a system connected to a supervising
station, the latter of which is not required by the building code. It's
a matter of education and theres nothing stopping a homeowner from
upgrading to NFPA-13 if property conservation is a concern.

We need to make sure that the message is clear, life safety.

John Drucker

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, March 31, 2008 12:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: U.S. Fire Administration Policy on Residential Sprinklers

Mike:
You are absolutely right! We should never expect more or lead anyone
else to expect more of a residential sprinkler system!
But in point of fact the actual real world data, suggests that the
residential sprinklers have performed beyond this design level in many
many instances. This does not mean we should expect that in every
installation, or condition. But it is a comfort to those of us that
layout these systems on a regular basis, that they do often out perform
our expectations. It's also the reason that many Fire Authorities
require that the supply exceed the 10 min. and be required to meet their
response time + 10 min. (The expect a structure to still be there when
they finally arrive.) It will always be difficult to explain after the
fire, that the sprinkler system did its job, especially if no one was
home, and the owner hasn't felt the personal risk he avoided, when all
he see's are his home and possessions in ashes.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: Mike Brown (TECH- GVL) [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, March 31, 2008 9:31 AM
Subject: RE: U.S. Fire Administration Policy on Residential Sprinklers


Just a note regarding residential sprinklers: I was in meetings of
various groups when the residential concept was first introduced.  The
concept was life safety and the preservation of life. Residential
sprinklers are designed and tested to give the occupants of the house or
dwelling ten minutes to get out of the house.  It was not intended that
residential sprinkler save a house or structure.  The objective was life
safety. Often I hear the words control and suppress used to describe
residential sprinklers which I believe to be incorrect.  Residential
sprinklers are life safety device that in many cases may control

RE: Sprinkler drop Tool

2008-03-27 Thread Mike Brown (TECH- GVL)
You can get one at Reliable.  It is called a SureOff Tester.  Contact your 
local Reliable representative.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel
Sent: Wednesday, March 26, 2008 9:57 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sprinkler drop Tool

Sounds like a hot tap tool and a strap on tapping saddle.

For example:  http://www.2lbin.com/ljr.htm and http://www.2lbin.com/
ts.htm

Allan Seidel
St. Louis, MO


On Mar 26, 2008, at 8:12 PM, Q.P. wrote:

 I was just wondering if anyone had seen a tool that  goes on a
 drop. It has a drill bit and a valve and guage.It is to make sure
 you have the right zone shut down.I had seen it once on  webpage
 and can not find it again. It seems like a tool every fitter should
 have.I know my guys would each get one.



Quentin Pahl / PahlFire

 Medicine Hat ,Alberta

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum-
 [EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Fire Systems and Plumbers/Last Thought

2008-03-26 Thread Mike Brown (TECH- GVL)
In response the Omega/GB problem has not gone away since there are probably 
thousands that have not been changed out or replaced.

If the industry is really serious about ensuring the residential systems work 
just mandate the Put the Water in the Bucket test and do an on the site test 
that the system delivers the correct water to the remote sprinklers.  It is my 
understanding that Upnor does that with each system that is installed.  When 
the Put the Water in the Bucket test was first introduced in Cobb County, GA 
there were quite a few systems installed by sprinkler contractors that did not 
pass the test.  Residential systems should be field tested to insure that the 
installation will provide the water and pressure required.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, March 26, 2008 10:48 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Fire Systems and Plumbers/Last Thought

I was going to add to Greg's submission that, theoretically (?), there should
be an AHJ both reviewing 'shop' drawings/calc's AND doing a rough-in 
final inspection to check for 'compliance' whether sprinks or plumbers are doing
the actual installation...That said, my biggest concern here in the State of
New Mexico is that we currently have 10 -12 Fire Extinguisher/Hood System
contractors that are (State) licensed to inspect, test, repair and INSTALL both
residential and commercial fire sprinkler systems.

These are contractors that somehow got into the sprinkler industry - for lack
of a better term - through the back door. My point being, many of them have
ZERO credentials - no NFSA/AFSA apprenticeship, no on-the-job training, no
training classes, zilch. They are now installing home fire sprinkler systems
in single-family dwellings in New Mexico. Pardon the 'pun', but (to me) some of
the plumbers are suddenly looking better.

Bottom line: We escaped the OMEGA/GB debacle with no loss of life (to my
knowledge)...With untrained, unsklilled, unethical PEOPLE installing residential
fire sprinkler systems, the loss of life - in sprinklered homes - is
inevitable. You read it here first.

Jerry D. Watts, SFPE
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe/Albuquerque, NM  Seattle, WA  San Diego, CA  Phoenix, AZ
e: [EMAIL PROTECTED]
web: www.accentfire.com
(800) 503.1961


**
Create a Home Theater Like the Pros. Watch the
video on AOL Home.

(http://home.aol.com/diy/home-improvement-eric-stromer?video=15?ncid=aolhom000301)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Interesting, but of little consequence

2008-03-26 Thread Mike Brown (TECH- GVL)
You may be hanging out with the wrong crowd.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - 
FPDC
Sent: Wednesday, March 26, 2008 12:09 PM
To: sprinklerforum@firesprinkler.org
Subject: Interesting, but of little consequence

Speaking of Omegas, I met a fitter this morning that had a tattoo of
an Omega sprinkler on his bicep.


At 11:47 AM 3/26/2008, you wrote:
In response the Omega/GB problem has not gone away since there are
probably thousands that have not been changed out or replaced.

If the industry is really serious about ensuring the residential
systems work just mandate the Put the Water in the Bucket test and
do an on the site test that the system delivers the correct water to
the remote sprinklers.  It is my understanding that Upnor does that
with each system that is installed.  When the Put the Water in the
Bucket test was first introduced in Cobb County, GA there were
quite a few systems installed by sprinkler contractors that did not
pass the test.  Residential systems should be field tested to insure
that the installation will provide the water and pressure required.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dry Pipe Valve going wet

2008-03-19 Thread Mike Brown (TECH- GVL)
In the tripped mode the water would be flowing out the alarm line to the bell 
or pressure switch.  The clapper would be in the latched position. If the 
clapper is not latched and is on the seat the water column probably would 
prevent it from operating.  This could be a dangerous situation.  In the south 
some plants like to take the clapper out and leave the system wet in the summer 
but I am not sure how they handled the alarm. In Europe they use wet/dry valve 
systems that are trimmed to allow the system to be alternated wet or dry 
depending on the season.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Larrimer, Peter A
Sent: Wednesday, March 19, 2008 4:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Dry Pipe Valve going wet

Forum Members:

If a dry pipe valve trips and goes wet, is there any reason why you
couldn't leave the system piping filled with water assuming that the
weather is not cold enough to freeze it?  I am assuming that the
clappers have been reset externally and that the alarm connections
remain dry since they don't seem to be having problems at this time.

Why would they want to use an alarm valve in place in liew of just
leaving the dry pipe valve?

Thanks in advance.

Peter Larrimer
VA


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
In years past staggered spacing was required in extra hazard applications.  At 
that time you only had 1/2 (5.6K) and 3/4 (8.0K) sprinklers. You may also find 
some 3/4 pipe used on old pipe schedule systems.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez
Sent: Wednesday, March 12, 2008 3:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe scheduled systems - head stagger

I have a retrofit of a system put in in 1963 where the heads on the
branch lines are staggered.  What was the reasoning for this back then?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Residential Upright

2008-03-12 Thread Mike Brown (TECH- GVL)
The Reliable F1 Res 49 is listed for an 8 inch deflector distance but the 
problem with all residential sprinklers is that they are not listed for 
obstructed construction which you may find in an attic.  NFPA 13D addresses it 
by saying that you can install pendent residential basements where it is 
expected that a ceiling will be installed or something like that.  To my 
knowledge there is no residential upright sprinkler made.  In my opinion you 
are better off using a Quick Response Commercial Upright sprinkler.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dennis J Briggs 
Jr.
Sent: Wednesday, March 12, 2008 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Residential Upright

Thanks Ron that may work for me.

Dennis Briggs, Jr.
Miller Fire Protection Inc.
2750 Marble Ct.
Forestville MD. 20747
Office - (301) 736-3000
Cell - (240) 304-8967
-Original Message-
From: Fletcher, Ron [mailto:[EMAIL PROTECTED]
Sent: Wednesday, March 12, 2008 01:13 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Residential Upright

I don't know of an upright but I think Globe makes a residential pendent listed 
for 8 or 12 deflector distance, I can't remember for sure. We have used them 
in loft style exposed systems because of the problem achieving the 4 deflector 
distance listed for most residential heads. Good luck. Ron Flecher Aero 
Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Dennis J Briggs Jr. Sent: Wednesday, 
March 12, 2008 5:37 AM To: sprinklerforum@firesprinkler.org Subject: 
Residential Upright Does anyone know if there is a Listed Residential Sprinkler 
Head currently on the market and if so where i may find it. Thanks, Dennis 
Briggs, Jr. Miller Fire Protection Inc. 2750 Marble Ct. Forestville MD. 20747 
Office - (301) 736-3000 Cell - (240) 304-8967 
___ Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, 
send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
field) ___ Sprinklerforum mailing 
list Sprinklerforum@firesprinkler.org 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, 
send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
No in the past before calculations there was a requirement in NFPA 13 to 
actually space the sprinkler in a staggered pattern rather than the way we 
space them today. Normally you would have ten foot spacing and the starter 
pieces in each line were done such that the sprinklers on one line were 
staggered so that the sprinklers on the next line were on the half space.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: Wednesday, March 12, 2008 3:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pipe scheduled systems - head stagger

When you say 'staggered' you mean a single row of pendants being fed off of
two rows (staggered) of upright piping?  If this is the case I would think
it would be merely for keeping pipe size down on each BL. Instead of taking
7 pendants, for example, off of one of the lines and having a lot of 2 inch
they might have tried to split it up and keep the line sizing down to 1 1/4
or 1 1/2 eliminating the need for 2.

Just my .02 cents. I've considered doing something similar to a
hydraulically calc'd system I'm working on right now.



On 3/12/08, Dewayne Martinez [EMAIL PROTECTED] wrote:

 I have a retrofit of a system put in in 1963 where the heads on the
 branch lines are staggered.  What was the reasoning for this back then?
 Thanks,
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
When I started in 1971, I think that we were only doing stagger spacing for 
extra hazard but if you have a 1961 NFPA 13 that is a treasure and there are 
not many left around.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Autry
Sent: Wednesday, March 12, 2008 4:00 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe scheduled systems - head stagger

Because that's they way the code reads.
My 1961 Edition
Light hazard need not be staggered, except under open wood joist. All others
shall be staggered.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Wednesday, March 12, 2008 2:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe scheduled systems - head stagger

In years past staggered spacing was required in extra hazard applications.
At that time you only had 1/2 (5.6K) and 3/4 (8.0K) sprinklers. You may
also find some 3/4 pipe used on old pipe schedule systems.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, March 12, 2008 3:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe scheduled systems - head stagger

I have a retrofit of a system put in in 1963 where the heads on the
branch lines are staggered.  What was the reasoning for this back then?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Ordinary chemical plants?

2008-03-06 Thread Mike Brown (TECH- GVL)
In Vietnam we used White Phosphorus bombs (known as Willie Pete).  You
cannot put it out with water.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rosemary
Beers
Sent: Thursday, March 06, 2008 3:57 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ordinary chemical plants?

My son just did his chemistry report on Phosphorus - his mobile had a
tube
of toothpaste on it.  Some phosphorus can not even be transported other
than
in water.  Out of water well - you do not want to be anywhere near.  Yet
it
is some toothpastes.

Point well taken.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, March 06, 2008 1:38 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ordinary chemical plants?


Toothpaste,  uh, you'd die if you knew some of the stuff that goes into
making some of our non-hazardous household products.   

Pharmaceuticals can use some highly toxic and flammable materials in the
process if not in the actual commodity.  Some of the chemicals used are
used to cause certain reactions and are then discarded and not actually
part of the end product but they are in the process.  That's why you've
got to know the process not just the end product.

Some pharmaceuticals and food products have used acetone, hot oils, heat
transfer fluids (class III's) above their flash points, ethylene oxide,
and the list goes on.  

Again it's hard to make any assumptions when it comes to these kinds of
facilities.  

So while a chemical plant could be OH2, they are kind of like unicorns.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Thursday, March 06, 2008 2:11 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ordinary chemical plants?

There could be chemical plants that are OH2. Say a plant manufacturing
medical drugs. That would also be a chemical plant. If the processed
material and products are non-hazardous, it could be OH2. Say a plant
that manufactures toothpaste. I have no clue regarding materials
involved. But if they are non-hazardous, could qualify for OH2. NFPA 45
for chemical laboratories classify labs OH1 and OH2 depending on the lab
classification.
The key is what are the material involved?

Tony   

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: March 6, 2008 11:15 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Ordinary chemical plants?

I'm glad to see others seem to be thinking along the same lines. This is
the second design-build chemical facility project this year with no
engineering or insurance company input and no company policies on fire
protection other than 'code says we need sprinklers'.

Let me pose this: if there is no such thing as an 'ordinary chemical
plant'
and they all require specific engineering analysis per NFPA 30, is NFPA
doing a disservice by including this in 13? Anybody can read that
statement and decide that a facility is an ordinary chemical plant and
protect it as
OH2 when it should be analyzed and could be a lot higher. Don't mean to
dis the sprinkler bible, but this type of statement could have some
unintended consequences.


At 12:07 PM 3/6/2008, you wrote:
I have never done a chemical processing facility that fell under NFPA
13 and never an OH occupancy. Usually they fall under NFPA 30 or a more

stringent and specific FM criteria.  Each plant requires a detailed 
hazards analysis of the process, equipment types and purpose, MSDS info

as well as building construction among other issues to determine the 
proper protection approach.

The other issue is that there are new technologies being born every
day.
Each new product being used or produced doesn't always have a page of 
it's own in the code.  So it takes some homework and detailed analysis 
when it comes to determining fire protection criteria for these kinds 
of facilities.

Ya gotta love it!


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd 
Williams - FPDC
Sent: Thursday, March 06, 2008 11:26 AM
To: sprinklerforum@firesprinkler.org
Subject: Ordinary chemical plants?

In NFPA 13, under the section describing OH2 occupancies, they mention 
Chemical plants - ordinary. What is an ordinary chemical plant?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080

RE: Dormitory Bunk Beds

2008-02-26 Thread Mike Brown (TECH- GVL)
Years ago I made all of the arguments that I see you making and the old
Fire Marshal in Florida said fine if you do not put a sprinkler under
the top bunk I will not give you a CO. END OF STORY.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, February 26, 2008 4:17 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dormitory Bunk Beds

Tim,

I think it is addressed clearly in 8.5.5.3.2 which states that 
Sprinklers shall not be required under obstructions
that are _not_ fixed in place such as conference tables.  (emphasis 
mine) I would think you could make an
excellent case that bunk beds are not fixed in place.  I agree that 
locating the sprinkler so that it might discharge
from the adjacent wall would be a reasonable approach, however I think 
you hit it on the head when you
mentioned that the furniture is movable.


PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website



G. Tim Stone wrote:
 I have asked an interesting question today by a general contractor and
need
 some assistance.

  

 A local college dormitory is undergoing some renovations and the
question
 was asked about double or full size Bunk Beds (wider than 4'-0) being
used
 in the rooms.

 The local fire marshal has asked about sprinkler protection below the
upper
 bunk. I am assuming an existing structure at this point and the design
will
 call for HSW sprinklers on exposed pipe.

 My thought would be to locate the sprinkler head on the opposite wall.
Now
 keep in mind that the furniture may be movable. 

  

 I do not believe this scenario is addressed in NFPA 13, 13R or D.
Platforms,
 Cutting tables and duct wider than 4' are addressed.

  

 Any thoughts or comments would be greatly appreciated.

  

 Thank you.

  

 G. Tim Stone

  

 G. Tim Stone Consulting, LLC 

 NICET Level III Engineering Technician

 Fire Protection Sprinkler Design

 and Consulting Services

  

 117 Old Stage Rd. - Essex Jct., VT. 05452

 TEL: (802) 434-2968  Fax: (802) 434-4343

 [EMAIL PROTECTED]

  


   



 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)



 No virus found in this incoming message.
 Checked by AVG Free Edition. 
 Version: 7.5.516 / Virus Database: 269.21.1/1298 - Release Date:
2/25/2008 8:45 PM
   
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
Check The International Building Code which requires sprinklers protecting some 
decks and in that section the IBC allows deviations from NFPA 13 or the 
sprinkler listing.  Maybe some bleed over into exterior canopies.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Thursday, February 21, 2008 5:44 PM
To: sprinklerforum@firesprinkler.org
Subject: Dry HSW under open framed 2x's

I'm noticing a lot of small exterior canopies being protected with dry 
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24 o/c) 
without any type of material fastened to the underside of this framing - which 
is all good and well since it mostly complies with NFPA #13 '07 ed section 
8.4.2 except that it's not 'SMOOTH.' So I guess that's my question, they aren't 
smooth so how are people getting away with this? Smooth being defined as 
sructural members being spaced more than 7'-6 o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a 
*pendant* at a 45 degree angle to protect small unheated areas so if it's okay 
for a pendant why not a HSW? (I'm sure it has to do with the intracacies of 
unfamiliar testing and listing requirements of a pendant over a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed as 
follows: 
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where specifically 
listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small 
unheated areas can be protected by dry-pendent sprinklers extending through the 
wall from wet sprinkler piping in an adjacent heated area. Where protecting 
covered platforms, loading docks, and similar areas, a dry pendent sprinkler 
should extend down at a 45 degree angle. The width of the area to be protected 
should not exceed 7½ ft (2.3 m). Sprinklers should be spaced not over 12 ft 
(3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as used 
in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced 
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or 
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses spaced 
more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on metal 
lath or a combination of materials of equivalent fire-resistive rating attached 
to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids, 
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that specified 
under item (d) and attached to the underside of wood joists, wood trusses, and 
bar joists 

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)


See the June 2006 Edition of Sprinkler Age in the article Balconies and the 
IBC by Steve Rians.

Mike Brown




-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple 
(forum)
Sent: Friday, February 22, 2008 9:51 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

To all

Looking at A.8.14.7 in 13 (02 ed), it looks like you are allowed to angle (@
a 45ºangle) a dry pendent through the wall without regard to construction
type. What would be the downside to doing this with a sidewall? (Other than
it does not show an HSW in the picture) Wouldn't the spray pattern develop a
little better?

Ken Holsopple
Rowe Sprinkler Systems, Inc.


I'm noticing a lot of small exterior canopies being protected with dry
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question,
they aren't smooth so how are people getting away with this? Smooth being
defined as sructural members being spaced more than 7'-6 o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's
okay for a pendant why not a HSW? (I'm sure it has to do with the
intracacies of unfamiliar testing and listing requirements of a pendant over
a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows: 
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat
ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where
specifically listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small
unheated areas can be protected by dry-pendent sprinklers extending through
the wall from wet sprinkler piping in an adjacent heated area. Where
protecting covered platforms, loading docks, and similar areas, a dry
pendent sprinkler should extend down at a 45 degree angle. The width of the
area to be protected should not exceed 7½ ft (2.3 m). Sprinklers should be
spaced not over 12 ft (3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as
used in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses
spaced more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on
metal lath or a combination of materials of equivalent fire-resistive rating
attached to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids,
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that
specified under item (d) and attached to the underside of wood joists, wood
trusses, and bar joists 

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email 

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
There are two issues with a sprinkler.  Those are sensitivity and distribution. 
 The sidewall sprinklers must be tested to insure that they provide the 
appropriate sensitivity and distribution in distribution tests (RDD  ADD) as 
well as sensitivity tests and fire tests.  I would not think that having a fire 
official just deciding one was better than the other is a really good idea.  
That smacks of the fire inspector saying he wants something done just because 
he wants it that way.  

Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, February 22, 2008 9:20 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

There seems to be a consensus among the inspector's I know that the sidewall
is better than a pendent in many cases because of the spray pattern. Would
there be a significant difference in the time it takes to fuse the two
different types of heads?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Friday, February 22, 2008 7:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

Check The International Building Code which requires sprinklers protecting
some decks and in that section the IBC allows deviations from NFPA 13 or the
sprinkler listing.  Maybe some bleed over into exterior canopies.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Sent: Thursday, February 21, 2008 5:44 PM
To: sprinklerforum@firesprinkler.org
Subject: Dry HSW under open framed 2x's

I'm noticing a lot of small exterior canopies being protected with dry
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question,
they aren't smooth so how are people getting away with this? Smooth being
defined as sructural members being spaced more than 7'-6 o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's
okay for a pendant why not a HSW? (I'm sure it has to do with the
intracacies of unfamiliar testing and listing requirements of a pendant over
a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows: 
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat
ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where
specifically listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small
unheated areas can be protected by dry-pendent sprinklers extending through
the wall from wet sprinkler piping in an adjacent heated area. Where
protecting covered platforms, loading docks, and similar areas, a dry
pendent sprinkler should extend down at a 45 degree angle. The width of the
area to be protected should not exceed 7½ ft (2.3 m). Sprinklers should be
spaced not over 12 ft (3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as
used in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses
spaced more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on
metal lath or a combination of materials of equivalent fire-resistive rating
attached to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids,
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that
specified under item (d) and attached to the underside of wood joists, wood
trusses, and bar joists 

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
That has been in NFPA 13 for ages but in 37 years I have never seen on done 
that way.  
Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple 
(forum)
Sent: Friday, February 22, 2008 9:51 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

To all

Looking at A.8.14.7 in 13 (02 ed), it looks like you are allowed to angle (@
a 45ºangle) a dry pendent through the wall without regard to construction
type. What would be the downside to doing this with a sidewall? (Other than
it does not show an HSW in the picture) Wouldn't the spray pattern develop a
little better?

Ken Holsopple
Rowe Sprinkler Systems, Inc.


I'm noticing a lot of small exterior canopies being protected with dry
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question,
they aren't smooth so how are people getting away with this? Smooth being
defined as sructural members being spaced more than 7'-6 o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's
okay for a pendant why not a HSW? (I'm sure it has to do with the
intracacies of unfamiliar testing and listing requirements of a pendant over
a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows: 
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat
ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where
specifically listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small
unheated areas can be protected by dry-pendent sprinklers extending through
the wall from wet sprinkler piping in an adjacent heated area. Where
protecting covered platforms, loading docks, and similar areas, a dry
pendent sprinkler should extend down at a 45 degree angle. The width of the
area to be protected should not exceed 7½ ft (2.3 m). Sprinklers should be
spaced not over 12 ft (3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as
used in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses
spaced more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on
metal lath or a combination of materials of equivalent fire-resistive rating
attached to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids,
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that
specified under item (d) and attached to the underside of wood joists, wood
trusses, and bar joists 

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL 

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
Yes George



George;

I was at the NFPA 13D meeting before the 2007 Edition of NFPA 13 came out and I 
went with one purpose and that was to discuss the questions that I get all of 
the time as a technical service manager.  What do I (designer or engineer) do 
when I have a sloped ceiling more than 8 in. in 12 in. and what do I do it the 
sloped ceiling that also has beams.  Additionally what do I do (designer or 
engineer) do I do when have a bunch of decorative beams creating pockets.  Is 
it good fire protection to put 16 residential sprinklers in a room with beams 
and only calculate two sprinklers?  I was not allowed to speak because I was 
not a member of the committee so I packed my bags and went home.  I know that 
there are a lot of opinion about everything but it was really difficult to 
watch some of the members who really did not seem to know a lot about 
sprinklers but were there to protect their turf. My opinion was that put they 
could put in the code that there that you have to treat it like light hazard or 
whatever (say calculate six sprinklers) but give the designers and engineers 
some direction.  What they did was dumped it back on the sprinkler designer or 
his company or the engineer and mostly the AHJ.  In my opinion the committee 
abdicated their responsibility.  There are also some other areas that need 
attention.  The voted to allow dry and Preaction systems in single family 
homes.  I answer questions all of the time about Preaction systems from 
sprinkler contractors that do more kinds of sprinkler systems than residential. 
 Many residential sprinkler contractors do not know anything about Preaction 
nor have they ever done a Preaction system.  Some of the people seemed to think 
that you could use the normal detectors in a home spaced any way you wanted to 
or that you would need a releasing panel. The reason was one of the members had 
a client that had ten million dollars worth of art and was concerned about 
accidental discharge.  In my opinion if you have ten millions dollars worth of 
art you do not need a 13D sprinkler system.  Another issue was not addressed 
and that is there is no limitation on the size of a single family home.  In my 
opinion a 44,000 square foot home does not need a 13D system. 
Another question is why do we not require and alarm on a 13D sprinkler system. 
The answer was the cost. That is BS since an electric bell is not expensive and 
yet they pass dry and Preaction. 

Overall, I was embarrassed and somewhat ticked off at the rampant attempts of 
certain parties to get the code changed to meet a product they either made or 
wanted to make. But that may be had it has always been.

All of this may be a moot point when you see the flows and pressures that are 
going to be required to pass the new UL testing requirements for residential 
sprinklers.

The insanity continues!

The above is my personal opinion and is not way intended to be the opinion of 
my company. 

Sorry that I got carried away but that is the way I feel.

Mike Brown 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Friday, February 22, 2008 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

Mike-
Were you at James' seminar at last AFSA where he had the sloped nightmare
residential scenarios in which heads in the hall opened before the otherwise
obvious heads that would open first? With the thermal movie?

My point is this-
James was completely surprised at which heads opened under beamed sloped
ceilings. He has a lot more testing experience than I'll ever have, even if
I quit and went to work for FM or UL tomorrow.

BUT- when deciding how to protect these buggers, we're to consult with and
seek direction from - the AHJ. Who likely has never seen a burn, probably
has never seen a burn video, let alone understand heat flow across beams or
along slopes, etc. if James was wrong, how do we think the AHJ is going to
be right? Law of averages, at least its either right or wrong and 50% is
better than what we'd otherwise get?

Mike, I AGREE WITH YOU that asking the local AHJ, who in my area may not
know what a flow switch looks like, is silly if you want an informed answer.
But isn't that what the Code directs us to do?

Scary, isn't it? Good thing we don't use spkrs as often as car brakes,
there's be more fire deaths.

Glc


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Friday, February 22, 2008 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

There are two issues with a sprinkler.  Those are sensitivity and
distribution.  The sidewall sprinklers must be tested to insure that they
provide the appropriate sensitivity and distribution in distribution tests
(RDD  ADD) as well as sensitivity tests and fire tests.  I would not think
that having a fire official just deciding one

RE: Parking Garage Sprinkler System

2008-02-01 Thread Mike Brown (TECH- GVL)
If you would like one I will send you a copy of my Rules of Thumb for
designing large dry systems.  You can contact me off line at
[EMAIL PROTECTED]
MLB

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Thursday, January 31, 2008 11:17 AM
To: sprinklerforum@firesprinkler.org
Subject: Parking Garage Sprinkler System

Hi All,
  I would like to ask about sprinkler system design in a car parking
garage. The parking garage has two stories (Basement  Ground floor). It
is only for car parking application which can hold about 350 cars.
  There is No mechanical devices to transport cars, and cars will drive
to their own parking palaces.
  The area of each story is about 44,000 square feet, and ceiling high
is about 10 feet.
  We are going to design a dry pipe sprinkler system for this car
parking garage as piping are subjected to freezing during the cold
weather.
   
  I looked up in NFPA codes for designing car parking garage, but I
couldn't find that much helpfull information in NFPA-88A.
   
  In NFPA-13 I saw that automobile parking and showrooms are specified
as 
  Ordinary hazard occupancies (Group 1).
   
  I am going to design a tree dry pipe sprinkler system  some inside
fire hoses in the garage.
   
  My questions are as followings:
   
  1- What is your recommended Area of sprinkler operation and Density
for my application after determining from the Density/Area curve?
   
  2- I am going to use upright sprinklers, what kind of sprinkler is
more common for such an application? standards coverage/extended
coverage...?
   
  3- What is the common distance between sprinklers and maximum area of
coverage per sprinkler for a parking garage?
   
  4- Is it necessary place a sprinkler exactly at above each car or not?
   
  5- Is it necessary to place sprinklers in corridors  ramps where no
cars are parked and only cars are moving?
   
  6- What is the NFPA recommended duration for sprinkler system  inside
hose stream?
   
  7- Can I connect the inside hose to the dry sprinkler system piping?
or shoud I connect the inside hose piping directly to the fire pumps?
   
  8- I will place some insde fire hoses in the garage that provides 1
1/2 in. hose stations and according to NFPA-14 the minimum residual
pressure at the outlet of most remote 1 1/2 in. hose stations should be
65 psi for hydraulically designed systems, so I think my fire pump head
should be at least 80 psi? What do you think about this fire pump head,
do you think it is low, high or good?
   
  9- I want to protect both strories with a single riser using a 4 dry
pipe system to feed my sprinkler system  fire hoses, what do you think
about it?
   
  Thanks for your kind help in advance,
  Reza
   

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo!
Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Mike Brown (TECH- GVL)
Reza
Take a look at your available pressure and choke down your branch line
sizes and look at your cross main and feed main sizes as well.  If you
can reduce them this makes the system volume less as well as makes the
system more economical.  If you have a lot of pressure and the structure
will allow it use extended coverage sprinklers.  If you expand your
spacing you will need more pressure but you will be covering more square
feet.  It is a game you play with pressure when designing systems and if
you can achieve the balance of the options you will have designed the
best system. Remember that NFPA 13 does not impose any velocity limits
but usually you need to say below 32ft per second.  The selection of the
k factor of the sprinkler is a part of the dance.  Generally, the large
the orifice in the inspector's test connection is the faster you can
exhaust the air from the system.

Good Luck
Mike Brown

By the way, those are Rules of Thumb not engineering principles and
you may at times make a different decision.  But those Rules of Thumb
are time tested over many years and if you violate all of them you can
have .

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili  
Sent: Friday, February 01, 2008 10:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Parking Garage Sprinkler System ***

Thanks Craig,
  As I am connecting fire hoses to my sprinkler system, then the system
pressure would be high to comply with NFPA-14 minimum residual pressure
requirements at the outlet of most remote 1 1/2 in. hose station which
is 65 psi. In this case my fire pump minimum head would be around 100
psi. Actually this pressure is good for the fire hoses but may be high
for my sprinkler system.
   
  As my required density is 0.15/1950 sq. ft which low, and my residual
pressure is high in my sprinkler system, then may be a sprinkler with
K=2.8 could work well to supply my required density, if I assume the
pressure in the most remote sprinkler is about 70 psi then:
  Q=k x sq. root of Pressure
  Q= 2.8 x sq. root of (70)
  Q= 23.4 GPM which is good and can supply my required density.
   
  But Mike sent me an article which stated Avoid 5.6 K-factor
Sprinklers.  Use Large Orifice (8.0 K-factor) or larger Sprinklers to
Exhaust the Air Faster.
   
  IF I use 8.0 K-factor then:
   
  Q=k x sq. root of Pressure
  Q= 8 x sq. root of (70)
  Q= 67GPM which is very large and much more than my required density
and will force me a big pump and a big water source!
   
  What should I do to solve this problem?
   
  Thanks,
  Reza
  

[EMAIL PROTECTED] wrote:
  Depending on where your riser is in relation to the remote part of
your
system you may have to have multiple systems to deal with the time
factor. It's a bit hard to determine without actually seeing everything
you're seeing. 

Make the electrical guy move his lights, tell him fire protection is
more critical. Maybe he will move, maybe you will have to work around
him. 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Friday, February 01, 2008 9:40 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Parking Garage Sprinkler System ***

Dears friends Craig, Travis, Kurt  Todd,
Many thanks for your detailed answer, your answers were very helpful,.
I will use the sprinkler piping for my fire hoses to save some pipe,
after calculation, the water velocity in piping is about 20 ft/s and the
capacity of sprinkler piping in each floor is 1030 gallons, so it seems
that each floors needs 2 dry pipe systems (As NFPA limits the volume of
a dry pipe system to 750 gallons).
***I know that this 750 gallons limit may be exceeded if the maximum
water delivery time is less than 60 seconds, I will use accelerators to
speed the operation of dry pipe systems, but I don't think even the
accelerators can reduce it to 60 seconds because the system is large,
what do you think? Do I have to use 2 dry pipe systems for each floor?
Is there any solution to use only 1 dry pipe system for each floor as I
want to be economical? Even if I don't connect fire hoses to sprinkler
piping, the system is large enough and it doesn't help that much, any
ideas?

*** Another question is that, the garage lighting system is about 50
cm below the roof, can I place the sprinklers above the lighting? I
think this is a kind of obstruction, what should I do? should i change
the place of lighting system?

Thanks,
Reza


[EMAIL PROTECTED] wrote:
Reza,


1- What is your recommended Area of sprinkler operation and Density for
my application after determining from the Density/Area curve? 
ANSWER: .15/1500 works but don't forget to increase the design area by
30% due to it being a dry 

RE: Max Ceiling Heights

2008-01-29 Thread Mike Brown (TECH- GVL)
Hi
There are no restrictions in NFPA 13 for Standard Spray Sprinklers.  The
ceiling limitations are for storage sprinklers like ESFR.  The old NFPA
101 Life Safety used to allow you to eliminate sprinklers in atriums
above 55 feet in height. There have been times when this has been
questions in the NFPA meetings but to my knowledge there have been no
new requirements added in NFPA 13.

Michael L Brown
The Reliable Automatic Sprinkler Company, Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, January 29, 2008 10:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Max Ceiling Heights

Craig,
Thanks for the input, the manufacturer just called me back and said they
have no limitations on the heads I'm using, I had him send me that in an
email which I will forward to the AHJ. 


Brian Harris
FDFP INC.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Max Ceiling Heights

Certain types of sprinklers have specific limitations and they are
usually
listed as such, typically those designated for storage occupancies.
Most
Control Mode sprinklers don't list any restrictions and so far I haven't
been able to find anything in NFPA stating an NFPA imposed restriction.
NFPA defers to the mfgr data for installation issues.

Dealt with this issue ad naseum on a 100ft high structure.   I contacted
one of the Sprinkler mfgrs and they were very helpful in explaining that
in
my case even at 100ft the sprinklers will operate.  The fire does have
to be
large enough to bring the ceiling temps up to the release temps of the
heads
and that could take a little longer than in a 20-30ft high bldg and
might
trigger more heads.  

If the AHJ is being persistent, ask the mfgr to write a letter
explaining
the operation of the heads at the higher elevation will occur and
whatever
other blah, blah blah words they need.  

Just something to satisfy the AHJ.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, January 29, 2008 9:43 AM
To: sprinklerforum@firesprinkler.org
Subject: Max Ceiling Heights

Forum,
I just got back some comments from the local AHJ on a project we are
doing
and he's asking me to verify that the heads we are using are rated for
ceilings over 30'. I've spoke with the manufacturer and he said he
doesn't
have anything on min./max. ceiling heights. If memory serves me isn't
50'
somewhere in NFPA? Any help would be appreciated.
 

Regards,

  http://www.firstdefensefire.com/ 

 

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: ESFR Pressure Anomaly

2007-12-11 Thread Mike Brown (TECH- GVL)
Understood and agree. 

My point is that testing and engineering can be used as a tool but do not throw 
out the baby with the bath water.  Some of the old guys that wrote NFPA 13 were 
quite good.  

I forgot Polybuthlene and PozLock piping which were listed and tested etc. but 
were removed from the market.  There are probably more that I cannot remember.

Mike Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Monday, December 10, 2007 5:34 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: ESFR Pressure Anomaly

Mike,

My point is that NFPA 13 should be read literally rather than being 
interpreted on the basis of assumptions about the depth and breadth of 
testing that may or may not be true, depending on the application. 13 is 
not defective, but some of the interpretations of it  are.

Joe



Mike Brown (TECH- GVL) wrote:
 Before you get too excited about the engineering process and testing I offer 
 the following:

 In the early 70's, GEM (Not called Tyco then) had a HSW that covered 16 x 28 
 ft. It was UL Listed until they figured out that they did not test it with a 
 ceiling.  When they did, the water spray hit the ceiling about mid-way and 
 never got to 28 ft.  It quietly disappeared from the market place.

 In the early 80's or there about there was the Central, and I think Grinnell, 
 On and Off head was tested and listed by UL until it too quietly 
 disappeared from the market place.

 Even lately there was an antifreeze system that was pushed by Tyco and FM as 
 well as a PHD at FM that was installed in a number of places until it too was 
 quietly removed from the market place. 

 There was also the Central Super Valve that disappeared from the market 
 place.

 And I do not even have to bring up the Omega and the GB which were the 
 greatest screw up of them all 

 There are others if I had time to list all of them.

 Many of the rules and regulations in NFPA 13 have stood the test of time in 
 the market place and too just dismiss these out of hand is a mistake. 

 Too many times based on a few fire tests we have, as an industry, jumped on 
 the band wagon and the wagon ran into a ditch along the way.

 Michael L. Brown

 -Original Message-
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
 Sent: Monday, December 10, 2007 2:12 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: ESFR Pressure Anomaly

 Thom-
 If you're a contractor- and I know you don't just play one on TV :)- 
 You're a risk-taker. In this litigious society, you can be held liable for
 meeting the adopted standard, but not applying a newer code. Or, for that
 matter, the reverse. So even with staying within the boundaries of adopted
 standards and codes does not relieve you of risk - and I know you and Noreen
 work hard at reducing and controlling the risks you have. And there are no
 right answers, but there certainly are wrong ones!

 If you're the first to take the test and you show up with K25's and 50
 PSI, you've got a pretty good shot at knocking down a challenge. Certainly
 not everything, and perhaps it could have been done with less- but at mega
 cost to continue running iterations of continually decreasing pressures.

 Heck, Thom, if I didn't feel lucky I wouldn't do what we do. Spent last Wed
 in depositions trying to collect money almost 3 years after a job completed.

 And certainly adopting good practices in advance of them being required is a
 way to both reduce risk and offer something of value to your customers. 

 We'll keep doing work under both the adopted standards and the Equivalency
 clause, dotting on I's, crossing our t's, because the stuff that blindsides
 us is often independent of the design criteria, and it can come down to the
 layman or judge (non-expert in either case) and their opinion on what was
 presented, not what SHOULD be, what COULD be, or what actually was.

 I was flabbergasted to learn about the old area/density curve development
 we've relied on for years- in a late-night war stories session at an AFSA
 convention (yes, that's a plug, how many places are you going to run into a
 discussion on this topic at 2 AM, and still be able to get drinks after
 hours to keep the discussion, well, moving?). I'd placed a lot more
 credibility on these graphs, and sweated out calcs to the 3rd decimal point,
 to find out they were derived- well, arbitrarily isn't far off the mark.

 glc

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
 Sent: Monday, December 10, 2007 1:50 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: ESFR Pressure Anomaly

 The main point James has made for class I-IV, is that the lower end of the 
 curve, may actually work most of the time, but as soon as you try to rise up

 the curve the greater the risk of failure. (Tyco has this nice test facility

 where he can play, and see things that have

RE: Most Remote Point

2007-12-11 Thread Mike Brown (TECH- GVL)
If you are interested I have a document that I call Rules of Thumb for
designing large dry systems that might be helpful.  Not engineering but
just old time rules that I learned at Automatic many years ago.  If
you will send me your email address at [EMAIL PROTECTED]  I
will be happy to share them.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Tuesday, December 11, 2007 11:45 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Most Remote Point

Ron,

We were always concerned about delivering water in no more than 1 
minute. (The 30% dry system penalty was based 1 minute delivery)  The 
assumption in 13 was that a 500 gal system (or 750 with an accelerator) 
would meet that requirement. Turned out to be a bad assumption. 

This also turned out to be another example of reading more into 13 than 
was intended.  People saw long water delivery times on systems with 
accelerators, and drew the conclusion (and I've seen it actually 
published) that a 10 minute delivery time was OK on a 750 gal system 
with an accelerator.  That's why the change is coming.

(I always was amazed that fire protection professionals could say a 5 
minute water delivery time was OK for a 750 gal system with an 
accelerator, but that an 800 gal system had to meet the 1 minute time. 
How dies the fire know the air capacity of the system)

A good rule of thumb, by the way, is to put the inspectors test 
connection on the end of the longest branch line at the end of a single 
cross main system ,and at the end of the longest branch line at the end 
of the cross main with the greatest air capacity (measured from the top 
of the riser) in multiple cross main systems.

The test connection should never be on a cross main.  The old trick used

to be to put the test connection on the bottom of a cross main at the 
end of the system. I saw a system (grid) deliver water to a test 
connection on the bottom of the cross main at the end of the system in 
45 seconds. A test connection in the middle of the remote grid line took

over 7 minutes.

Joe

 Bill,

 How important is this? Until yesterday we were only concerned that the
 system tripped (which in reality would have left the IT anywhere since
 the air decompresses evenly) and that there was no debris in the
 system which would work its way to the opening. Oh and that water
 delivery was within a minute on systems over 750 gallons. Now (or
 coming soon to a code near you) we have the minute for everything but
 just how important is it we get that remote point down to the one and
 only most remote by seven inches point? I still get to use skill,
 experience and my magic eight ball for the design area. I still use
 water data taken at a particular time and on a particular day by
 instruments with a pretty loose degree of accuracy measuring a
 constantly changing fluid in motion as universally accurate and then
 perform calculations that employ constants and ignore issues like
 temperature, viscosity and gravity. How accurate can any of this be.
 With all due respect, and you know I hold you in high regards, this
 sounds like an academician's  question.

 On Dec 11, 2007 5:07 AM,  [EMAIL PROTECTED] wrote:
   
 Is there a way to prove that a dry system inspector's test is in the
 most remote position?  Can this be demonstrated by some sort of
 calculation?

 Bill Brooks

 William N. Brooks, P.E.
 Brooks Fire Protection Engineering Inc.
 372 Wilett Drive
 Severna Park, MD 21146
 410-544-3620 Phone
 410-544-3032 FAX
 412-400-6528 Cell

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 



   

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: ESFR Pressure Anomaly

2007-12-10 Thread Mike Brown (TECH- GVL)
Before you get too excited about the engineering process and testing I offer 
the following:

In the early 70's, GEM (Not called Tyco then) had a HSW that covered 16 x 28 
ft. It was UL Listed until they figured out that they did not test it with a 
ceiling.  When they did, the water spray hit the ceiling about mid-way and 
never got to 28 ft.  It quietly disappeared from the market place.

In the early 80's or there about there was the Central, and I think Grinnell, 
On and Off head was tested and listed by UL until it too quietly disappeared 
from the market place.

Even lately there was an antifreeze system that was pushed by Tyco and FM as 
well as a PHD at FM that was installed in a number of places until it too was 
quietly removed from the market place. 

There was also the Central Super Valve that disappeared from the market place.

And I do not even have to bring up the Omega and the GB which were the greatest 
screw up of them all 

There are others if I had time to list all of them.

Many of the rules and regulations in NFPA 13 have stood the test of time in the 
market place and too just dismiss these out of hand is a mistake. 

Too many times based on a few fire tests we have, as an industry, jumped on the 
band wagon and the wagon ran into a ditch along the way.

Michael L. Brown

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, December 10, 2007 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: ESFR Pressure Anomaly

Thom-
If you're a contractor- and I know you don't just play one on TV :)- 
You're a risk-taker. In this litigious society, you can be held liable for
meeting the adopted standard, but not applying a newer code. Or, for that
matter, the reverse. So even with staying within the boundaries of adopted
standards and codes does not relieve you of risk - and I know you and Noreen
work hard at reducing and controlling the risks you have. And there are no
right answers, but there certainly are wrong ones!

If you're the first to take the test and you show up with K25's and 50
PSI, you've got a pretty good shot at knocking down a challenge. Certainly
not everything, and perhaps it could have been done with less- but at mega
cost to continue running iterations of continually decreasing pressures.

Heck, Thom, if I didn't feel lucky I wouldn't do what we do. Spent last Wed
in depositions trying to collect money almost 3 years after a job completed.

And certainly adopting good practices in advance of them being required is a
way to both reduce risk and offer something of value to your customers. 

We'll keep doing work under both the adopted standards and the Equivalency
clause, dotting on I's, crossing our t's, because the stuff that blindsides
us is often independent of the design criteria, and it can come down to the
layman or judge (non-expert in either case) and their opinion on what was
presented, not what SHOULD be, what COULD be, or what actually was.

I was flabbergasted to learn about the old area/density curve development
we've relied on for years- in a late-night war stories session at an AFSA
convention (yes, that's a plug, how many places are you going to run into a
discussion on this topic at 2 AM, and still be able to get drinks after
hours to keep the discussion, well, moving?). I'd placed a lot more
credibility on these graphs, and sweated out calcs to the 3rd decimal point,
to find out they were derived- well, arbitrarily isn't far off the mark.

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Monday, December 10, 2007 1:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: ESFR Pressure Anomaly

The main point James has made for class I-IV, is that the lower end of the 
curve, may actually work most of the time, but as soon as you try to rise up

the curve the greater the risk of failure. (Tyco has this nice test facility

where he can play, and see things that have not been tested for FM or UL 
approval, just the increased knowledge of TYCO and their staff)
We are risk takers. Our insurance companies are risk takers, with Attitude. 
And our owners believe that we have removed all of their risk. Increasing 
our exposure because its allowed has never been appealing to me, and each of

us shouldn't wait for it to be Code before we adopt good practices. So 
before you climb up that curve, ask yourself Do Ya Feel Lucky?

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message - 
From: Chris Cahill [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, December 10, 2007 11:12 AM
Subject: RE: ESFR Pressure Anomaly


I was reading from the cut sheet, technically FM criteria.  NFPA according
to the cut sheet there is no protection scheme for the K25.  Even in the
table you reference there is no ESFR 25 for this.

As far as flows 25's 

RE: Tape and/or Dope

2007-12-07 Thread Mike Brown (TECH- GVL)
This may stem from the CPVC people who say do not both tape and dope
the thread  It has always been done with steel pipe but with CPVC it
can cause problems.
Mike Brown.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Friday, December 07, 2007 2:07 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tape and/or Dope

I think the point is to tape and dope the inspector ...

Steve Leyton
Protection Design  Consulting


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gary
Stites
Sent: Friday, December 07, 2007 8:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Tape and/or Dope

Here's one for you

In Los Angeles on a high-rise building, we had a field inspector cite
NFPA 13, 6-5.1.3 (2002) as meaning we could use tape OR compound on pipe
NOT both.  Does anyone out there believe this is the intent of the code?
Or do you think the point of this passage is to NOT put these items on
the female threads? 

Gary Stites
Operations Manager: Southern California
RLH Fire Protection
3430 Unicorn Road
Bakersfield, Ca. 93308
661-322-9344 #1343
Direct Line 661-410-1343
Direct FAX 866-871-2237
[EMAIL PROTECTED]
www.rlhfp.com
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Maximum Velocity

2007-11-14 Thread Mike Brown (TECH- GVL)
I guess being old and having been around for a long time.  The 32 ft per
sec came from some old water distribution engineering manuals and became
sort of a rule of thumb for sprinkler calculations in that when you get
above that velocity the friction loss gets larger in a hurry.  At one
time FM came out with a requirement for a maximum of 20ft per second in
grid branch lines but they sort of backed off on that issue but did keep
the requirement for the velocity in riser nipples or something like
that.  I am not sure what FM does now regarding velocity.  Most of the
computer hydraulic programs have followed the old rule of thumb that you
need to keep your velocity at or under 32 ft per second and usually they
will show you the various pipes that exceed that velocity and you can
make the decision on changing the pipe size or not. But the velocity is
not addressed in NFPA 13.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 14, 2007 3:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Maximum Velocity

also look at 13: A.22.4.1 (last sentence) It is not necessary to  
restrict the water velocity when determining friction loss using the  
Hazen-Williams formula.

This is also in the 02 edition.

Roland

On Nov 12, 2007, at 6:41 AM, Brian Harris wrote:

 What's the general rule of thumb for maximum velocities in  
 hydraulic calc's?
 I use Hydra-Calc and the default is set @ 32, I assume that's feet per
 second. Where did that number come from, I didn't see anything in  
 the code
 book.


 Regards,

   http://www.firstdefensefire.com/




 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Supervisory Alarm - Low Air

2007-11-05 Thread Mike Brown (TECH- GVL)
The monitoring of a high pressure is not in NFPA 13 or any other NFPA
Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit
to put it in NFPA 13.  I have never met anyone that could tell me why it
was in NFPA 72.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Wednesday, October 24, 2007 9:58 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Supervisory Alarm - Low Air

Of course! How foolish of me! Dave, can you send me your address. I
lost it and I want to send your Tacoma Code Book.

On 10/24/07, David de Vries [EMAIL PROTECTED] wrote:
 How would you know?  Simple, Ron.  You would just check the log where
the building engineer dutifully recorded the air pressure on the system
on a weekly basis, as required by NFPA 25 where there is no electrical
supervison, of course!

   lol

   Dave at Firetech Engineering Incorp.

 Ron Greenman [EMAIL PROTECTED] wrote:
   I've always considered the high air supervision more critical than
low
 since a malfunctioning compressor that runs the air up will cause a
 longer trip time whereas low air will just let you know that an
 unwanted trip could happen if not attended to. Of course the emphasis
 is put on the low air because that trip rolls fire trucks, requires a
 technician to be summoned, disrupts the normal course of a day and
 costs the owner money. All recordable events and therefore
 statistically useful for proving one point or another. If, on the
 other hand, you receive a high air you just fix the problem as a piece
 of equipment that needs maintenance. If a life or building was ever
 lost because of high air delaying a trip how would anyone ever know?
 The evidence would demonstrate an overwhelmed system but although it
 might suggest it there is nothing I can think of that would
 definitively demonstrate it was due to a delayed trip time. If a bear
 s in the woods...?

 On 10/24/07, Tim Frankenberg wrote:
  Dave,
 
  The requirement to monitor low and high air pressure has been in the
code before the 1993 edition of the National Fire Alarm Code.
 
  Most of the supervisory pressure switches installed are very much
capable of monitoring both low and high air and have been able to for
many, many years. More times than not, the high air condition is not
being enforced by the AHJ.
 
  Kind Regards,
 
  Tim Frankenberg, CFPS
 
  Tim Frankenberg, CFPS
  Fire Product Manager
  Potter Electric Signal Company
  www.pottersignal.com
  800-325-3936
 
   Dave Phelan 10/23/2007 4:52 PM 
  Something new to me popped up today as we are now using the 2002
editions of
  13  72 here.
 
  On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72
states that
  the air supervisory sensor shall signal on loss of 10 PSI but also
on 10 PSI
  greater than the system set pressure. Check out 5.13 for yourself
but I'm
  thinking Ive never seen or tested for air greater than 10 PSI of the
set
  pressure before.
 
  How is this being handled in the field during installs and
maintenance ?
  Does the typical air pressure switch in the little red cover
actually cover
  both loss and increase pressures?
 
  Thanks.
 
  Dave - a NJ AHJ
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
to:[EMAIL PROTECTED]
  (Put the word unsubscribe in the subject field)
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  To Unsubscribe, send an email
to:[EMAIL PROTECTED]
  (Put the word unsubscribe in the subject field)
 


 --
 Ron Greenman
 at home
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)



-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: RE:Clean room sprinkler heads w/ covers

2007-11-05 Thread Mike Brown (TECH- GVL)
Just for your info.  Reliable still makes a Sealing  Concealer with a
gasket but it is not quick response or FM Approved.  Check the Reliable
website www.reliablesprinkler.com
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Cabral
Sent: Tuesday, October 30, 2007 10:10 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: RE:Clean room sprinkler heads w/ covers

What you describe sounds like a sprinkler that was made by ASCOA
Automatic Sprinkler Company of America As far as I know they are long
gone. It was there standard concealed sprinkler with a silicone gasket
that attached to the cover plate to provide a seal between the space
above the sprinkler and the clean room.

Mike Cabral

 Ford wrote: 
 A customer is asking us to provide sprinklers for a clean room. We saw
some installed ones and they
 appear to have very large cover plates that are rubber gasketed at the
ceiling. Manufacturer unknown.
 Anybody run into these and knows their origin?
 
 
 Burton Ford
 SET, CFPS
 Member AFAA
 [EMAIL PROTECTED]
 267-487-1000
 Fax 267-487-1010
 
 This e-mail transmission contains information that is intended to be
confidential and privileged.  If
 you receive this e-mail and you are not a named addressee you are
hereby notified that you are not
 authorized to read, print, retain, copy or disseminate this
communication without the consent of the
 sender and that doing so is prohibited and may be unlawful.  Please
reply to the message immediately
 by informing the sender that the message was misdirected.  After
replying, please delete and otherwise
 erase it and any attachments from your computer system.  Your
assistance in correcting this error is
 appreciated.  Thank you.  Cintas Corporation
 
 
 
 
 This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not
a named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be
unlawful.  Please reply to the message immediately by informing the
sender that the message was misdirected.  After replying, please delete
and otherwise erase it and any attachments from your computer system.
Your assistance in correcting this error is appreciated.
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 To Unsubscribe, send an email
to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dry system size

2007-10-11 Thread Mike Brown (TECH- GVL)
Let me say again, you might want to check with the AHJ because many of
them and some of the building codes still requiring a one head test and
you must get the water to the ITC in 60 seconds.  You can engineer it
all you want but it will boil down to what the code and the AHJ
requires.
Michael L. Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, October 11, 2007 12:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Dry system size

reread the last sentence of 7.2.3.7. for confirmation of what I said

Roland

On Oct 11, 2007, at 8:50 AM, Russell wrote:

 So if I choose option #3, I do not have to use option #2 involving  
 a program
 or use #1 and meet it's requirement of a single connection with 60  
 sec. time
 period. #3 means using a test manifold using table 7.2.3.6.1. This  
 table
 shows (in my situation for ordinary hazard) to use a two outlet  
 manifold
 utilizing one branch line and a water delivery time of 50 seconds.

 Ron



 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Roland
 Huggins
 Sent: Thursday, October 11, 2007 11:16 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Dry system size

 lets start over again and allow me to summarize what has been said by
 others.

 For systems greater than 750 gals, you have THREE options.
 1. Single test connection at 60 seconds
 2. Calculated delivery using Table 7.2.3.6.1
 3. Test manifold using Table 7.2.3.6.1

 Read 7.2.3.7 taking note of the last sentence (confirming if you use
 the manifold you do not have to do either of the other two options).
 This section also tells you where to connect when more than 2
 sprinklers are on the manifold.

 Other tidbits:
 Even with a calculated system, you still have to do the single head
 flow test as part of the acceptance test BUT there is NO 60 sec limit.
 For smaller systems serving a dwelling unit, you now have to satisfy
 the 60 sec rule (for spray sprinklers).

 Roland

 On Oct 10, 2007, at 1:45 PM, Russell wrote:

 I take it that the table 7.2.3.6.1 goes only with a program, but if
 so, how
 do I determine the number of branch lines to include in the
 manifold? Am I
 not understanding what you're telling me?

 Ron

 Internal Virus Database is out-of-date.
 Checked by AVG Free Edition.
 Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:
 6/10/2007
 1:39 PM


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum-
 [EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 Internal Virus Database is out-of-date.
 Checked by AVG Free Edition.
 Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:  
 6/10/2007
 1:39 PM


 Internal Virus Database is out-of-date.
 Checked by AVG Free Edition.
 Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:  
 6/10/2007
 1:39 PM


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Dry system size

2007-10-10 Thread Mike Brown (TECH- GVL)
You might want to check the building codes.  Some require that the
system meet the 60 second rule no matter what the volume of the dry
system is.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Wednesday, October 10, 2007 4:15 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry system size

Yes, if over 750 gallons.  Under 750 you still get the choice of the
quick
opening device with time not mattering and under 500 time doesn't matter
-
no manifold no program.  The time could be as low as 40 sec. depending
on
the hazard.  See 7.2.3.1 in the '07. Table 7.2.3.6.1 goes with it.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Wednesday, October 10, 2007 2:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry system size

Uh oh, so you're saying that I will need to use the manifold and meet
the 60
seconds when I'm not using a program?

Ron 

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:
6/10/2007
1:39 PM
 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Spare Head boxes

2007-09-17 Thread Mike Brown (TECH- GVL)
There was one of the after market providers that used to have a
plastic sprinkler head box.
ARCO or FPPI ??
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete
Schwab
Sent: Monday, September 17, 2007 11:39 AM
To: sprinklerforum@firesprinkler.org
Subject: Spare Head boxes

Does anyone know of a spare head box that can stand up to a corrosive
environment?
Standard head boxes that are available as a standard do not do well
against direct exposure to the elements.
Any help/advice is appreciated
Pete Schwab


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into The Players Hall of Fame
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. Best Places to Work
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Bucket Test

2007-09-13 Thread Mike Brown (TECH- GVL)
Folks
The  Put the Water in the Bucket Test was developed years ago when
Cobb County GA Fire Department was promoting what later became NFPA 13R.
The Cobb County Fire Dept. was promoting an affordable fire sprinkler
system in commercial and residential applications.   There was a video
produced by Byron Belzak to show how to conduct a bucket test.  I know
because I was a paid actor in the video.  You would be surprised to
learn that a lot of the systems installed when tested did not provide
the correct amount of water out of the remote sprinkler.  The bucket
test was a way to actually test the systems prior to covering up the
system piping.  I would suggest that you contact the Cobb County, GA
Fire Department and they may be able to supply more information.
Another contact would be Jerry Grier, now retired, at (678) 517-8938.

Michael L. Brown
The Reliable Automatic Sprinkler Company

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Thursday, September 13, 2007 9:32 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Bucket Test

 
They get you by the whatever by refusing to sign off on the system so
you
can't get a certificate of occupancy and the general contractor the
architect  the owner go ballistic, so you do what Dum-Dum wants.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, September 13, 2007 4:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Bucket Test

Pete has an excellent idea about showing where the committee rejected
proposals to 13R; Far easier to ask where the requirement stems from- So
you
can completely comply with the provisions of the alleged requirement-
And
when he can't find the requirement, you don't need to do it.

If he says he wants it even tho he can't produce the requirement, ask
him if
it isn't done, what would be the penalty?
Under what secition of applicable law would you be prosecuted?

glc
 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete
Schwab
Sent: Wednesday, September 12, 2007 8:31 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Bucket Test

The bucket test has been around for a long time. May have originated in
Cobb
County - then again, I do not know for sure.
The best thing you can do to convince the AHJ that it is not necessary
is to
go back to the report on Proposals and Comments for NFPA 13R. I BELIEVE
IN
THE 90'S. There have been proposals to the committee requiring the
bucket
test that have been rejected.
If the AHJ won't buy this, you have to call it the cost of doing
business
(unfortunate but true)

Pete Schwab
Wayne Automatic Fire

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Pie Pans

2007-08-30 Thread Mike Brown (TECH- GVL)
Yes, contact the AFSA and the NFSA.  I believe that Roland Huggins did
an article on it and I know Russ Fleming of the NFSA did one years ago.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Thursday, August 30, 2007 12:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Pie Pans


Okay, forum.
I know pie pan heat collectors don't work and actually make it worse.
My question, is there any documentation that I can get my hands on? 

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Test

2007-06-11 Thread Mike Brown (TECH- GVL)
OK

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Monday, June 11, 2007 10:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Test

It was a slow Friday. 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tambini,
Ed
Sent: Monday, June 11, 2007 8:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Test

WTF???!!! 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Friday, June 08, 2007 3:30 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Test

Let's see, have you ever told a lie?  What do you call a person who
tells a
lie?  If I told you a lie, what would that make me? A liar.
Have you ever taken anything that did not belong to you?  What do you
call a
person who takes things that do not belong to him / her?  If I took
something from you, what would you call me?  A thief.
When we compare ourselves to the Ten Commandments, which give us a
picture
of God's perfection, we see that we don't stack up too well.
Now that's a good test to see how we will do on the day we stand before
God.

To take the test yourself follow the link, http://www.needgod.com/


Bob Knight

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Smith,
Steven
D. (CSFD)
Sent: Friday, June 08, 2007 3:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Test

What is the criteria to determine if it's a good test or not? 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Friday, June 08, 2007 1:07 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Test

That was a good test. 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray
Schmid
Sent: Friday, June 08, 2007 7:08 AM
To: sprinklerforum@firesprinkler.org
Subject: Test

 

 

Ray Schmid, P.E.

Principal

Koffel Associates, Inc.

410-750-2246

www.koffel.com http://www.koffel.com/ 

This communication is confidential. This information may be privileged
and
is intended for the exclusive use of the above named addressee(s).
If you are not the intended recipient(s), you are expressly prohibited
from
copying, distributing, disseminating, or in any other way using any of
this
information contained herein. If you have received this communication in
error, please contact the sender by telephone at (410)
750-2246 or by response via e-mail and then permanently delete the
original
email and any copies.

 

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.472 / Virus Database: 269.8.9/832 - Release Date: 6/4/2007
6:43 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.472 / Virus Database: 269.8.9/832 - Release Date: 6/4/2007
6:43 PM
 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Adobe Structures

2007-05-09 Thread Mike Brown (TECH- GVL)
Dear Ed 
You may want to talk to the NFPA 13 D Committee that in the 2007 Edition
allowed the use of dry and preaction systems in residential occupancies.
There is no doubt that the old reliable wet system is the least likely
to need maintenance etc. but how many fires have not been controlled by
systems with the control valves shut.  

Nothing is fool proof and double interlock preaction systems that are
designed correctly, installed correctly and maintained properly work
quite well in thousands of installation.  

You want real heart burn think about residential installations where
preaction systems are installed by companies that rarely do preaction
and maintained by the home owner.

Mike Brown


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining
Sent: Wednesday, May 09, 2007 3:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Adobe Structures

Ed, don't listen to the hydrophobic hysterical architect.  These
historic adobes have been around for decades.  Many were run down, had
lost their roofs, and were exposed to the elements for years.  Now look
at them.
 
Second piece of advice, don't be fooled by the so-called advantages of
preaction systems.  They are complicated, and much less reliable than
ordinary wet-pipe systems.  In structures like these, unreliability
includes both in failure to operate, and operation when there is no
fire.  Witness what happened at the new planetarium at the College of
San Mateo.  Reports say accidental discharge of this system ruined the
planetarium equipment.  A similar event occurred at TV station KQED.
Testing of a preaction system at Pine Hall, Stanford University caused a
leak, and damaged vital computer equipment.  Failure of a preaction
system in Fresno resulted in a million dollar fire loss in a warehouse.
 
In the real estate business it's location, location location.  With
sprinklers it's wet pipe, wet pipe, wet pipe
 
[EMAIL PROTECTED]
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792 



- Original Message 
From: Ed Cyr [EMAIL PROTECTED]
To: American Fire Sprinkler Association
SprinklerFORUM@firesprinkler.org
Sent: Wednesday, May 9, 2007 11:55:42 AM
Subject: Adobe Structures


Forum Members,

The Great State of California has many historic missions that are made
of
adobe (dried mud bricks). Wood roof structure.
Our county has adopted an ordinance that all buildings in our downtown
core
be sprinklered by a certain date in the future.

We have seen written comments from a preservation architect that has
worked
on numerous historic adobe buildings, that fire sprinklers should not be
installed in any historic adobes.

This recommendation is based on inherent risk of water damage.

I recommended that a dbl interlock pre-action system would suffice. That
would take care of the accidental activation issue.

Question: Does anyone have a case history of dealing with adobe
structures?
What is the forums opinion on how this should be treated?
Suggestions for alternate protection measures?

Any comments would be appreciated.

Thanks,
Ed Cyr

Alpha Fire Sprinkler Corp.
San Luis Obispo, CA

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: heat activated devices for a deluge system.

2007-03-29 Thread Mike Brown (TECH- GVL)
If the designer or engineer knew what he or she was doing there would be
a test valve in the pilot line to test the system.
Mike Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, March 29, 2007 3:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: heat activated devices for a deluge system.

I think they need to be a bit more specific in their reference to what
kind of pneumatic HAD's they have.  This could be construed as closed
sprinkler heads (pilot heads) on pilot piping.  

If they are using an electrical actuation utilizing something like the
Notifier 302 or similar series heat detector (HAD) then I would think
they should be tested as would any other actuation device of the fire
alarm system.

But I've never tested a pilot system by busting a pilot head open.

You've got different types of hardware that can be considered Heat
Activated Devices (heat detectors).   Often the application dictates the
type of device that will work best in the situation.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Eric
Shelton
Sent: Thursday, March 29, 2007 3:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: heat activated devices for a deluge system.

Since NFPA 72 includes discussion of these types of detectors, I'm not
sure the 72 committee would agree that since they're not electrical
they're not fire alarm.

The original question might get some additional answers from folks more
knowledgeable than I over at the firealarm yahoo-group.

Eric Shelton
Hankins and Anderson, Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, March 29, 2007 2:59 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: heat activated devices for a deluge system.

they are NOT electrical devices, so 72 shouldn't be part of the
equation.  The ones I've played with are just domes with small diameter
tubes.  Never thought of them as a pneumatic SIGNAL.  That may be
leading to some of the confusion.  Better to think of it as a pneumatic
HAD that activates the system.

As a related note, the current edition of 25 only checks the mechanical
condition of the electrical (72 type) activation  
components of a deluge system.  There is no requirement for a   
functional test of the electrical release side.  This will be addressed
in the 07 edition stating that a 72 inspection of those components is
required to ensure the system is full functional.  That is provided that
isn't one of the NITMAMs going to the NFPA floor in June.  I'm not
saying it was required.  It just wasn't driven by 25.

Roland

On Mar 29, 2007, at 11:29 AM, MOWLE Kevin(K) - BRUCE POWER wrote:



 Are heat actuated devices (HADS) used to initiate a deluge system via 
 a pneumatic signal considered:
 1- a heat detector and so the required testing is per NFPA 72 ?
 2- or are the HADS considered part of the deluge system so testing 
 requirements as per NFPA 25 ?

 Thanks

 Kevin Mowle
 Bruce Power
 Tiverton, ON

 guess
 **

 
 *** The contents of this email and any attachments
 *** are confidential and may be privileged.
 *** They are intended for the named recipient(s) only.
 *** If this message has been delivered to you in error, please reply 
 to the
 *** sender to that effect, don't forward the message to anyone
 *** and delete the message from your computer.
 *** Thanks for your help, and sorry for the inconvenience.
 **

 

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
 field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email

RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread Mike Brown (TECH- GVL)
Folks
A water hammer can do nasty things to a sprinklers system but just pump
pressure can cause problems if the sprinkler fitters have not done their
work properly.  Years ago at Phillips Plaza in Atlanta a grooved
coupling was not properly tightened because the groove on the pipe was
too shallow.   The grooved coupling held for the 200 psi test but later
when the pump was put into service the coupling did not hold and the
basement of the upscale mall was flooded and the complete mall was shut
down for several hours while the system was repaired.  Fortunately the
installers were not mine.

Michael L. Brown

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, March 09, 2007 10:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: What I'm Hearing About Hydrostatic Testing

more worried about it NOT staying in its intended orientation.

Joe - Did you guys see any systems where sprigs and rotated?

Roland

On Mar 8, 2007, at 7:01 PM, Joe Hankins wrote:

 There was nothing to suggest water hammer. Water hammer resulting  
 from a pump start is unlikely in sprinkler system piping. Even if   
 there is a water hammer problem, it's something you want to know  
 because it's easy to fiz.When you do see water hammer from a fire  
 pump, it usually happens in underground.

 Also, starting fire pumps with the discharge valve open is by far  
 the most common way weekly runs are made.  I've seen many sprinkler  
 systems that have held up to weekly pump starts for more than 30  
 years without incident.

 If you truly beleive that a sprinkler system can be blown apart by  
 a fire pump, you have a very low opinion of  the quality of  
 sprinkler installations!

 Joe