RE: Mixed rack storage

2018-11-29 Thread MFP Design, LLC
Don’t forget that depending on how your carpet squares and rolled rug are stored, that could create a “solid shelf” Travis Mack, SET, CWBSP MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: system modification hydro test

2018-11-15 Thread MFP Design, LLC
That’s funny. I believe that statement has been in the standard since before flex drops were even available. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: Deck and Balcony sprinklers

2018-11-08 Thread MFP Design, LLC
Your building is Type V construction. V-A and V-B just deal with ratings of the walls in certain areas. If you have Type V-A or V-B, you are putting sprinklers at the back areas. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Sprinklers next to Diffusers

2018-11-08 Thread MFP Design, LLC
Ask the mechanical engineer that did the HVAC plans. 8.3.2.5(9) may eliminate the issue. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: corridors and residential sprinklers

2018-10-29 Thread MFP Design, LLC
That pretty clearly shows 4 sprinklers in a corridor. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

corridors and residential sprinklers

2018-10-29 Thread MFP Design, LLC
calculate 4. To eliminate the 75' max argument, let's say the sprinklers are spaced at 16' on center. So, do we calculate 4 or 5 residential sprinklers in a corridor? This came up in a discussion today. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271

RE: 130 sq ft or 225 sq ft

2018-10-18 Thread MFP Design, LLC
It will have insulation. That may be how they got to 225 sq ft. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook

RE: Interstitial Sprinklers

2018-10-18 Thread MFP Design, LLC
You can use SxL. You don't have to do in 2' increments like with Ex Cov sprinklers. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

130 sq ft or 225 sq ft

2018-10-18 Thread MFP Design, LLC
rea. What does everyone think? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi g

RE: Converting from ESFR to CMDA - Spacing Issues

2018-10-08 Thread MFP Design, LLC
ery time we've dealt with this in the past, we have had to respace sprinklers along the branchline when that happens. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: Type V Construction & Hangers

2018-09-25 Thread MFP Design, LLC
I know you CA peeps do. I had just never run into it outside of CA. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.ou

Type V Construction & Hangers

2018-09-25 Thread MFP Design, LLC
this. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Tire Carousels

2018-09-21 Thread MFP Design, LLC
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166 77342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2F

RE: multi-height standpipes

2018-09-19 Thread MFP Design, LLC
I believe this is spelled out in the NFPA 14 handbook. You will need to do 2 sets of calculations. Where you only have 2 standpipes, you calculate the 750 gpm. When you get down to the level with 3 standpipes, you do another calc that goes to 1000 gpm. Travis Mack, SET MFP Design, LLC

RE: FM APPROVAL

2018-08-25 Thread MFP Design, LLC
https://www.approvalguide.com/CC_host/pages/public/custom/FM/login.cfm You just have to register Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: NFPA 13 Closet Definition

2018-08-20 Thread MFP Design, LLC
understanding. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Baffle for fire sprinkler system

2018-08-13 Thread MFP Design, LLC
Those are useless. There is no criteria because they are not permitted. If you need a water shield, use a listed sprinkler with water shield. If you need a “heat collector”, you are out of luck. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
There are many ways to address this. Some AHJs want us to reduce the curve off the top. Others want us to keep it as measured and maintain a minimum margin. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
Yes. It would be at the horizon for sure  Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
In this example… Apply a 10% reduction to the measured flow test results. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

Flow Test Reductions

2018-08-08 Thread MFP Design, LLC
way lately. Doing that has differing slopes and the lines would intersect. The theoretical reduction could actually have a higher pressure at a given flow with #2 since it is a flatter curve. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
Your description of accessible by more than one dwelling unit is exactly the way I view it. But, I got shot down by the AHJ. Their response was: “What if some one propped open a door?” Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d

NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
to the floor joists. We can be up in the joist space running parallel. So, CPVC or steel? What is the forum consensus? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: [EXTERNAL] System area limitations

2018-07-31 Thread MFP Design, LLC
Yes. I checked. There is nothing like that. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: System area limitations

2018-07-31 Thread MFP Design, LLC
I can’t tell you how many times I’ve wanted to send a bill to a plan reviewer titled “Education Expenses” Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

RE: System area limitations

2018-07-31 Thread MFP Design, LLC
ion. This guy is a “senior fire protection consultant” doing the review. There have been several comments along these lines. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpd

System area limitations

2018-07-31 Thread MFP Design, LLC
vis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f1

RE: HVLS Fan clearance

2018-07-27 Thread MFP Design, LLC
Maybe some one could do some model simulation on the effects of the fans, clearances ≤36”, sprinkler activation time and maybe a few other variables. I don’t know how one models the obstructions of the fan blades, but it may be possible. Travis Mack, SET MFP Design, LLC 3356 E Vallejo

RE: Paint Booths

2018-07-25 Thread MFP Design, LLC
Don't forget to apply NFPA 13: (2016) 23.4.4.2.4 and 23.4.4.2.5. That can make some of these smaller areas be a bit of an issue. The same thing is also in the 2013 edition as well. It is 23.4.4.1.1.4 and 23.4.4.1.1.5 in the 2013 edition. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct

RE: definition of public space

2018-07-25 Thread MFP Design, LLC
. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Flange Spacers?

2018-07-09 Thread MFP Design, LLC
It is just a short “main” with a size on size welded outlet. Don’t we do that all the time? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
Matt: I think Craig is dealing with some one that thinks if the calcs say you only “need” 40 psi at the base of riser, then that is all that the water supply will deliver. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightai

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
We all make mistakes and things happen. But, there does appear to be a huge gap in understanding some times. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

RE: Real system pressures versus the calculations

2018-06-27 Thread MFP Design, LLC
minimums. You can run supply calcs to determine what pressures and flows you can expect with the full water supply discharging. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> em

RE: [EXTERNAL] RE: % open

2018-06-25 Thread MFP Design, LLC
This is all steel construction. The exterior projection overhang is steel construction and the new add on to the clubhouse that this projects from is also steel construction. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: % open

2018-06-25 Thread MFP Design, LLC
Yes. That is exactly it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.

% open

2018-06-25 Thread MFP Design, LLC
, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d

RE: Ground Storage tank

2018-06-13 Thread MFP Design, LLC
It sounds like you are indicating you want to use a "brake tank." As long as you put an automatic fill valve on the tank, you can use the city supply to help reduce the quantity of stored water. You may want to check NFPA 22 for this. Travis Mack, SET MFP Design, LLC 3356 E

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
ESFR are not spray sprinklers and can not be interchanged to meet a density/area curve. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
8f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2F

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
I always try to contact the FM reviewer and ask for the table where they are getting the info in their datasheets. I then put that table on the drawings so there is no question as to where the criteria was derived. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298

RE: FM Mutual & ESFR Heads

2018-06-04 Thread MFP Design, LLC
for storage sprinklers. So, even though the 11.2 is just a standard spray sprinkler, you must adhere to all of the storage sprinkler obstruction and spacing criteria of the appropriate FM Datasheet. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: Ceiling Grids and Flex Drops

2018-05-30 Thread MFP Design, LLC
What was the final resolution?? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi

RE: ESFR closer than 8'

2018-05-30 Thread MFP Design, LLC
My understanding is the same as Don stated. It is not skipping or cold soldering. It is too many sprinklers opening. The baffle or curtain will do little, if anything, to alleviate that. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: Ceiling Grids and Flex Drops

2018-05-30 Thread MFP Design, LLC
Tell him they are UL Listed for use in fire sprinkler systems. He needs to prove that they can't be used. Call Victaulic. I would imagine they can get you something. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email

RE: Water Delivery Times

2018-05-18 Thread MFP Design, LLC
It is from the time the head opens as the way I understand it and had to meet requirements of. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Misc Rack Storage

2018-05-17 Thread MFP Design, LLC
When you have mixed criteria areas, you need to extend the higher density into the lower density area for 15’. Reference NFPA 13: 12.3 for that requirement. Also, don’t forget the issue of complying with 23.4.4.1.1.4. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ

RE: Strainer ahead of fire pump

2018-04-24 Thread MFP Design, LLC
It’s not required but is permitted. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpd

RE: Assembly or Not?

2018-04-20 Thread MFP Design, LLC
tion." Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDes

RE: Perpendicular to Slope / Attic

2018-04-17 Thread MFP Design, LLC
Yes. It is across the joist. 5' is a minimum. You can exceed it as long as your spacing limits are adhered to. Maybe 5' from one side and 6' from another to get away from the hip? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Expansion Joint

2018-04-11 Thread MFP Design, LLC
Yes. If you are in 9.3, you are doing seismic bracing. If you are Seismic Design Cat A or B, typically you are not going to do seismic and 9.3 with it's sub chapters would not apply. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

Floor Assemblies

2018-04-05 Thread MFP Design, LLC
ce with 8.15.1.2.6. It just seemed strange that there wouldn't be some other exception to eliminate sprinklers in that space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...

RE: NFPA-13 Chapter 17 Rubber Tires

2018-04-02 Thread MFP Design, LLC
Well, show him 18.2.4 and ask him for his understanding of that. Remind him location has meaning. Chap 17 is not for rubber tire storage. None of the criteria in Chap 17 applies to Chap 18. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866

RE: NFPA-13 Chapter 17 Rubber Tires

2018-04-02 Thread MFP Design, LLC
Chap 18 is rubber tires. 18.2.4 states that column protection is not required with ESFR. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: PVC drain line

2018-03-30 Thread MFP Design, LLC
for the drain lines. It is highly impractical from a cost perspective. Check in A3.2.1 in the 2016 NFPA 13 handbook if you have it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesi

RE: PVC drain line

2018-03-30 Thread MFP Design, LLC
. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F=0

RE: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ]

2018-03-28 Thread MFP Design, LLC
a replacement. However, 11.2k ex cov and 5.6k std cov have different thread sizes, so I think it would be quite challenging to get the sprinklers mixed up if you have to replace one. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: concealed space less than 6" deep

2018-03-28 Thread MFP Design, LLC
sq ft design area triggered. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com

RE: concealed space less than 6" deep

2018-03-28 Thread MFP Design, LLC
. I would lean back to 8.15.1.2.5 and keep sprinklers out of the space. But, you will need to increase the design area to 3000 sq ft for adjacent spaces. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:t

RE: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ]

2018-03-28 Thread MFP Design, LLC
6'x6' or something like that. I believe that AFSA did an informal interp on this and agreed with the position that using K5.6 std coverage and K11.2 ex cov (for example) is permitted, even in areas that do not comply with the small room rule. Travis Mack, SET MFP Design, LLC 3356 E

RE: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ] [EXTERNAL]

2018-03-28 Thread MFP Design, LLC
Well, when I have 4 sprinklers in a room at 18x18 and then another sprinkler protecting about 30 sq ft, putting in the 11.2k in that area causes enough of an over-discharge to change pipe sizing. So it can be rather significant at times. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct

FW: Case 00201286: Differing k-factors [ ref:_00D5077Vx._5005013w8og:ref ]

2018-03-28 Thread MFP Design, LLC
1 std cov sprinkler in the same room would not be acceptable. Am I reading this correctly? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417

CWBSD

2018-03-27 Thread MFP Design, LLC
. Anyway, I just wondered if anyone has heard much about it. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

30% increase for Sloped ceilings

2018-03-27 Thread MFP Design, LLC
What year did the 30% increase for sloped ceilings come into NFPA 13? I'm trying to do keyword search but no luck at this time. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> em

RE: AutoCAD Question

2018-03-23 Thread MFP Design, LLC
I would think it depends on your license type. Call your distributor and see if they can determine if you need to do anything special. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> em

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
opinion on the matter and the committee members were no better than him so their opinion didn’t carry any more weight. But, on the particular issue he told me that, he has since revised his stance. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
what it takes on stuff like this. It helps when the plan reviewer is actually a very nice person. He acknowledges that they take a different interpretation, and understands the other side, but this is what their department has arrived at. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
I was informed from the AHJ that they would accept a "technical question" answer from NFPA only if he agreed with it. Otherwise, it would take a formal interpretation. As I said, some days you just really have to love what you do. Thankfully I do. Travis Mack, SET MFP Design,

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
and life interesting. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign

RE: EC & SC

2018-03-22 Thread MFP Design, LLC
Oh, this is one of those AHJs that is heavy badged. 23.4.4.8 in the 2013 edition clarifies it. Much is in the handbook though. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https

EC & SC

2018-03-22 Thread MFP Design, LLC
it is acceptable to do this? I am almost certain it is clearly stated, but I can't find it this morning. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: stages

2018-03-15 Thread MFP Design, LLC
Do you run a separate standpipe system for the hose valves, or come off the overhead? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692

stages

2018-03-15 Thread MFP Design, LLC
off the overhead system and just add 50 gpm per hose valve for your inside hose requirements? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

Duct Sox / ESFR

2018-03-13 Thread MFP Design, LLC
Has anyone come across the duct sox and ESFR protection? How do you handle these? I intend to put a sprinkler under the duct as normally required. But, these somewhat vanish when the HVAC system is off. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271

RE: Residential Sprinklers

2018-03-06 Thread MFP Design, LLC
for area of sprinkler in 13R. So, you may have to choose the larger k factor residential sprinklers. We typically do a 4.9k pendent, but you may have to go to the larger ones depending on your requirements. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax

RE: Residential Sprinklers

2018-03-05 Thread MFP Design, LLC
You can only have a maximum of 4 QR sprinklers per dwelling unit, not just compartment. If you need more than 4 standard spray sprinklers, you can't comply with 13R. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com

RE: inrack sprinkler question

2018-02-23 Thread MFP Design, LLC
from 16.2.1.4.3.1 to the demand calculations for the ceiling sprinklers and balance to the higher of the two pressure demands to ensure that the water supply can handle the simultaneous operation of ceiling and in-rack sprinklers." Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert

RE: CFC 2016

2018-02-21 Thread MFP Design, LLC
than Bitcoin in 2017. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign

CFC 2016

2018-02-21 Thread MFP Design, LLC
sprinkler based on calculations * Edition of NFPA 13 We have to provide a copy of this sign on our plans. Additionally, we have to provide a copy of the General Information Sign on the plans. Things in CA get more and more unusual every year. Travis Mack, SET MFP Design, LLC

RE: [EXTERNAL] Re: ESFR Heads in Concrete Tee's

2018-02-16 Thread MFP Design, LLC
I think the issue is that ESFR sprinklers can’t be less than 8’. You can do <6’ with SSU/P sprinklers as the standard references baffles in those instances. ESFR is a different animal. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-

RE: QR/SR Sprinklers

2018-02-15 Thread MFP Design, LLC
that you have to use a listed SR K5.6 sprinkler in the space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?ur

RE: Sprinklerforum Digest, Vol 59, Issue 4

2018-02-13 Thread MFP Design, LLC
, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
not be able to deliver the needed water, but that is something different. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.ou

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
I didn't even read that. NFPA 13 uses nominal k-factors. There is no difference in a K17 and K16.8. Look in Chapter 6. You will see anything with a range of 16.0-17.6 is to be calculated at k16.8 Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505

RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread MFP Design, LLC
I believe you are going to be out of luck. As far as I know, Tyco is the only one that makes one. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Sprinkler in vertical duct

2018-02-07 Thread MFP Design, LLC
Dig into the areas of 13 about that. I don’t have the reference off hand, but you have provisions to use sprinklers in different orientations for the exhaust duct. So, just put a pendent sprinkler in the horizontal position. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert

RE: Institutional sprinklers in 13R

2018-02-07 Thread MFP Design, LLC
3. Can you justify the sleeping areas are the "dwelling units" and the corridors / kitchens / living rooms are the areas "outside the dwelling unit" so that you can apply 13R? Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 4

RE: Datasheet NFPA

2018-02-05 Thread MFP Design, LLC
www.nfpa.org <http://www.nfpa.org> They accept many different forms of payment. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com &

RE: 3-Hour Rated Walls

2018-02-02 Thread MFP Design, LLC
Make sure you can get a sleeve/caulk combo to give the 3 hour rating. That may be a challenge to find. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <htt

RE: Calculation of sprinklers under soffits

2018-01-24 Thread MFP Design, LLC
them to K4.2 or 2.8 if you are in a light hazard space. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=h

RE: S & L Rule

2017-12-21 Thread MFP Design, LLC
ways done it. I just see the reasoning behind the question. Does the answer change if you have a girder instead of a beam? Why or why not? Merry Christmas to all and to all a good night! Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-4

RE: S & L Rule

2017-12-21 Thread MFP Design, LLC
sprinklers to a line. It is generally more costly to add extra lines. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook

RE: [EXTERNAL] Multiple Pumps

2017-12-19 Thread MFP Design, LLC
I’ve had some large demand systems….5000 gpm and more. They always had specified (3) 2500 gpm pumps for the 5000 gpm systems. I had one 9000 gpm system that had (4) 3000 gpm pumps. The idea was that if any one pump was done, the system would still be maintained with adequate pumping

RE: Informal Interps

2017-12-19 Thread MFP Design, LLC
inion only, as a member of the NFPA 13 Technical Committee, and do not represent an official interpretation of the NFPA 13 standard. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, December 19, 2017 10:40 AM To: sprinklerforum

Informal Interps

2017-12-19 Thread MFP Design, LLC
knowing as the EOR. However, having the backing of the AFSA to our position, the EOR backed off of his incorrect interpretations and is going to be working on re-designing the issue in question. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430

RE: [EXTERNAL] RE: Protection under bleachers in a Gymnasium

2017-12-12 Thread MFP Design, LLC
f248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.high

RE: Underground Main Between 2 Attached Building Areas

2017-12-11 Thread MFP Design, LLC
, if there is an underground leak, you don’t have to take out the entire building. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook