RE: Nipple Extenders

2008-05-09 Thread Mike Brown (TECH- GVL)
United Brass makes a 1/2 by 1/2 male by female and a 3/4 x 3/4 male by female extender. These can be used to extend a drop that is cut too short. AFSA in the past had a BEST PRACTICE written about the use of these. There is some argument that these should not be used but they can be

RE: Return Bends

2008-05-08 Thread Mike Brown (TECH- GVL)
As I remember the return bend was to help insure that creeping crud and corrosion does not build up on the orifice inlet of the sprinkler and cause problems with the operation of the sprinkler. Or maybe I am just getting brain hiccups. Michael L. Brown Manager of Technical Services The

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Mike Brown (TECH- GVL)
My point is that the NFPA 13D Committee should provide guidelines to follow in these situations. I do not care if they say calculate the room to light hazard as long as they put it in writing. But the way it is now, it is just what ever the contractor or engineer (designer) can get the AHJ to

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Mike Brown (TECH- GVL)
The NFPA 13D Committee in their wisdom (or as some people have suggested lack thereof) put in the 2007 Edition Paragraph 8.1.3.1.2 Where construction features or other special conditions exist that are outside the scope of sprinkler listings, listed sprinklers shall be permitted to be

RE: What is a Bucket Test?

2008-04-24 Thread Mike Brown (TECH- GVL)
Actually, in several counties around Atlanta, the test was also required for garden style apartments up to four stories. You would be surprised that, at least in the beginning, a number of projects that had full blown hydraulic calculations failed when the bucket test showed them to be

RE: engineering decisions

2008-04-24 Thread Mike Brown (TECH- GVL)
, 2008, at 6:15 AM, Mike Brown (TECH- GVL) wrote: Actually, in several counties around Atlanta, the test was also required for garden style apartments up to four stories. You would be surprised that, at least in the beginning, a number of projects that had full blown hydraulic calculations failed

RE: engineering decisions

2008-04-24 Thread Mike Brown (TECH- GVL)
. It can't be done with just a copy of FM Data Sheets. Joe Mike Brown (TECH- GVL) wrote: Roland This will get you going---As usual the engineer does not want to do anything but get paid. Just write in the spec: [Sprinkler System as per NFPA 13 and all materials and design shall meet UL

RE: What is a Bucket Test? (TIA Needed)

2008-04-15 Thread Mike Brown (TECH- GVL)
Of Mike Brown (TECH- GVL) Sent: Monday, April 14, 2008 3:56 PM To: sprinklerforum@firesprinkler.org Subject: RE: What is a Bucket Test? (TIA Needed) I agree with Thom in that, as we are getting closer to mandated fire sprinklers in single family homes, the potential for a large number of new

RE: What is a Bucket Test?

2008-04-09 Thread Mike Brown (TECH- GVL)
I am sure if you contact the Cobb County Georgia Fire Department they will tell you about a lot of failures particularly when they first started. The local contractors know about the test and check it themselves before they call for an inspection. You guys are very diligent about your

RE: What is a Bucket Test?

2008-04-09 Thread Mike Brown (TECH- GVL)
You use the orifice size of the sprinklers that you are testing. You install full port ball valve in a drain pipe from each of the sprinklers you are testing with the correct orifice. If you contact Cobb County, GA you can get their procedures if you are interested. Michael L. Brown Manager

RE: U.S. Fire Administration Policy on Residential Sprinklers

2008-03-31 Thread Mike Brown (TECH- GVL)
on 13D's. Just wanted to make sure no confusion on that. John Drucker -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Monday, March 31, 2008 2:45 PM To: sprinklerforum@firesprinkler.org Subject: RE: U.S. Fire Administration Policy

RE: Sprinkler drop Tool

2008-03-27 Thread Mike Brown (TECH- GVL)
You can get one at Reliable. It is called a SureOff Tester. Contact your local Reliable representative. Michael L. Brown Manager of Technical Services The Reliable Automatic Sprinkler Company, Inc.' [EMAIL PROTECTED] www.reliablesprinkler.com (864) 843-5228 -Original Message- From:

RE: Fire Systems and Plumbers/Last Thought

2008-03-26 Thread Mike Brown (TECH- GVL)
In response the Omega/GB problem has not gone away since there are probably thousands that have not been changed out or replaced. If the industry is really serious about ensuring the residential systems work just mandate the Put the Water in the Bucket test and do an on the site test that the

RE: Interesting, but of little consequence

2008-03-26 Thread Mike Brown (TECH- GVL)
You may be hanging out with the wrong crowd. Michael L. Brown Manager of Technical Services The Reliable Automatic Sprinkler Company, Inc.' [EMAIL PROTECTED] www.reliablesprinkler.com (864) 843-5228 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd

RE: Dry Pipe Valve going wet

2008-03-19 Thread Mike Brown (TECH- GVL)
In the tripped mode the water would be flowing out the alarm line to the bell or pressure switch. The clapper would be in the latched position. If the clapper is not latched and is on the seat the water column probably would prevent it from operating. This could be a dangerous situation. In

RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
In years past staggered spacing was required in extra hazard applications. At that time you only had 1/2 (5.6K) and 3/4 (8.0K) sprinklers. You may also find some 3/4 pipe used on old pipe schedule systems. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]

RE: Residential Upright

2008-03-12 Thread Mike Brown (TECH- GVL)
The Reliable F1 Res 49 is listed for an 8 inch deflector distance but the problem with all residential sprinklers is that they are not listed for obstructed construction which you may find in an attic. NFPA 13D addresses it by saying that you can install pendent residential basements where it

RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
No in the past before calculations there was a requirement in NFPA 13 to actually space the sprinkler in a staggered pattern rather than the way we space them today. Normally you would have ten foot spacing and the starter pieces in each line were done such that the sprinklers on one line were

RE: Pipe scheduled systems - head stagger

2008-03-12 Thread Mike Brown (TECH- GVL)
Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Wednesday, March 12, 2008 2:50 PM To: sprinklerforum

RE: Ordinary chemical plants?

2008-03-06 Thread Mike Brown (TECH- GVL)
In Vietnam we used White Phosphorus bombs (known as Willie Pete). You cannot put it out with water. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Rosemary Beers Sent: Thursday, March 06, 2008 3:57 PM To: sprinklerforum@firesprinkler.org

RE: Dormitory Bunk Beds

2008-02-26 Thread Mike Brown (TECH- GVL)
Years ago I made all of the arguments that I see you making and the old Fire Marshal in Florida said fine if you do not put a sprinkler under the top bunk I will not give you a CO. END OF STORY. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
Check The International Building Code which requires sprinklers protecting some decks and in that section the IBC allows deviations from NFPA 13 or the sprinkler listing. Maybe some bleed over into exterior canopies. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
See the June 2006 Edition of Sprinkler Age in the article Balconies and the IBC by Steve Rians. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple (forum) Sent: Friday, February 22, 2008 9:51 AM To:

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
] On Behalf Of Mike Brown (TECH- GVL) Sent: Friday, February 22, 2008 7:47 AM To: sprinklerforum@firesprinkler.org Subject: RE: Dry HSW under open framed 2x's Check The International Building Code which requires sprinklers protecting some decks and in that section the IBC allows deviations from NFPA 13

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
That has been in NFPA 13 for ages but in 37 years I have never seen on done that way. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple (forum) Sent: Friday, February 22, 2008 9:51 AM To: sprinklerforum@firesprinkler.org

RE: Dry HSW under open framed 2x's

2008-02-22 Thread Mike Brown (TECH- GVL)
PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Friday, February 22, 2008 10:31 AM To: sprinklerforum@firesprinkler.org Subject: RE: Dry HSW under open framed 2x's There are two issues with a sprinkler. Those are sensitivity and distribution. The sidewall sprinklers must be tested to insure

RE: Parking Garage Sprinkler System

2008-02-01 Thread Mike Brown (TECH- GVL)
If you would like one I will send you a copy of my Rules of Thumb for designing large dry systems. You can contact me off line at [EMAIL PROTECTED] MLB -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Thursday, January 31, 2008 11:17

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Mike Brown (TECH- GVL)
Reza Take a look at your available pressure and choke down your branch line sizes and look at your cross main and feed main sizes as well. If you can reduce them this makes the system volume less as well as makes the system more economical. If you have a lot of pressure and the structure will

RE: Max Ceiling Heights

2008-01-29 Thread Mike Brown (TECH- GVL)
Hi There are no restrictions in NFPA 13 for Standard Spray Sprinklers. The ceiling limitations are for storage sprinklers like ESFR. The old NFPA 101 Life Safety used to allow you to eliminate sprinklers in atriums above 55 feet in height. There have been times when this has been questions in

RE: ESFR Pressure Anomaly

2007-12-11 Thread Mike Brown (TECH- GVL)
point is that NFPA 13 should be read literally rather than being interpreted on the basis of assumptions about the depth and breadth of testing that may or may not be true, depending on the application. 13 is not defective, but some of the interpretations of it are. Joe Mike Brown (TECH- GVL

RE: Most Remote Point

2007-12-11 Thread Mike Brown (TECH- GVL)
If you are interested I have a document that I call Rules of Thumb for designing large dry systems that might be helpful. Not engineering but just old time rules that I learned at Automatic many years ago. If you will send me your email address at [EMAIL PROTECTED] I will be happy to share

RE: ESFR Pressure Anomaly

2007-12-10 Thread Mike Brown (TECH- GVL)
Before you get too excited about the engineering process and testing I offer the following: In the early 70's, GEM (Not called Tyco then) had a HSW that covered 16 x 28 ft. It was UL Listed until they figured out that they did not test it with a ceiling. When they did, the water spray hit the

RE: Tape and/or Dope

2007-12-07 Thread Mike Brown (TECH- GVL)
This may stem from the CPVC people who say do not both tape and dope the thread It has always been done with steel pipe but with CPVC it can cause problems. Mike Brown. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Friday, December

RE: Maximum Velocity

2007-11-14 Thread Mike Brown (TECH- GVL)
I guess being old and having been around for a long time. The 32 ft per sec came from some old water distribution engineering manuals and became sort of a rule of thumb for sprinkler calculations in that when you get above that velocity the friction loss gets larger in a hurry. At one time FM

RE: Supervisory Alarm - Low Air

2007-11-05 Thread Mike Brown (TECH- GVL)
The monitoring of a high pressure is not in NFPA 13 or any other NFPA Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit to put it in NFPA 13. I have never met anyone that could tell me why it was in NFPA 72. Mike Brown -Original Message- From: [EMAIL PROTECTED]

RE: RE:Clean room sprinkler heads w/ covers

2007-11-05 Thread Mike Brown (TECH- GVL)
Just for your info. Reliable still makes a Sealing Concealer with a gasket but it is not quick response or FM Approved. Check the Reliable website www.reliablesprinkler.com Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Cabral Sent:

RE: Dry system size

2007-10-11 Thread Mike Brown (TECH- GVL)
Let me say again, you might want to check with the AHJ because many of them and some of the building codes still requiring a one head test and you must get the water to the ITC in 60 seconds. You can engineer it all you want but it will boil down to what the code and the AHJ requires. Michael L.

RE: Dry system size

2007-10-10 Thread Mike Brown (TECH- GVL)
You might want to check the building codes. Some require that the system meet the 60 second rule no matter what the volume of the dry system is. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Wednesday, October 10, 2007

RE: Spare Head boxes

2007-09-17 Thread Mike Brown (TECH- GVL)
There was one of the after market providers that used to have a plastic sprinkler head box. ARCO or FPPI ?? Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Pete Schwab Sent: Monday, September 17, 2007 11:39 AM To:

RE: Bucket Test

2007-09-13 Thread Mike Brown (TECH- GVL)
Folks The Put the Water in the Bucket Test was developed years ago when Cobb County GA Fire Department was promoting what later became NFPA 13R. The Cobb County Fire Dept. was promoting an affordable fire sprinkler system in commercial and residential applications. There was a video produced by

RE: Pie Pans

2007-08-30 Thread Mike Brown (TECH- GVL)
Yes, contact the AFSA and the NFSA. I believe that Roland Huggins did an article on it and I know Russ Fleming of the NFSA did one years ago. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Autry Sent: Thursday, August 30, 2007 12:07 PM

RE: Test

2007-06-11 Thread Mike Brown (TECH- GVL)
OK -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Monday, June 11, 2007 10:34 AM To: sprinklerforum@firesprinkler.org Subject: RE: Test It was a slow Friday. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: Adobe Structures

2007-05-09 Thread Mike Brown (TECH- GVL)
Dear Ed You may want to talk to the NFPA 13 D Committee that in the 2007 Edition allowed the use of dry and preaction systems in residential occupancies. There is no doubt that the old reliable wet system is the least likely to need maintenance etc. but how many fires have not been controlled by

RE: heat activated devices for a deluge system.

2007-03-29 Thread Mike Brown (TECH- GVL)
If the designer or engineer knew what he or she was doing there would be a test valve in the pilot line to test the system. Mike Brown -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, March 29, 2007 3:44 PM To:

RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread Mike Brown (TECH- GVL)
Folks A water hammer can do nasty things to a sprinklers system but just pump pressure can cause problems if the sprinkler fitters have not done their work properly. Years ago at Phillips Plaza in Atlanta a grooved coupling was not properly tightened because the groove on the pipe was too