RE: Plastic Tenting of CPVC

2006-11-13 Thread Craig.Prahl
Heat and cold can't see through black plastic. It makes the pipe invisible to fire and freezing. ;) One possibility is that they are going to insulate over the pipe and it would make it easier for the insulation to lay on top of the plastic instead of between the pipe and the rafters. Only prob

RE: Non listed sway bracing

2006-11-15 Thread Craig.Prahl
Check out TOLCO products. They have an array of seismic bracing options. One problem is the possible liability involved when someone says "they want something but it doesn't have to be listed", is whether you can assure them that the product used outside of it's intended purposes will actually pe

RE: Non listed sway bracing

2006-11-15 Thread Craig.Prahl
In plumbing systems you can have water hammer due to the quick on-off action of valves. You typically don't have that in sprinkler systems. Usually sprinkler flow would start with one head flowing or a nozzle opening. That won't create the kind of quick on-off action which would result in water h

RE: Non listed sway bracing

2006-11-16 Thread Craig.Prahl
If all this is typical for sprinkler systems, would one think the NFPA committees or FM would have addressed the issue due to historical data revealing system failures or damage from "water hammer" or hydraulic shock? While we can pontificate until sunrise and beyond, I can't find any directive t

RE: audible alarm

2006-11-16 Thread Craig.Prahl
When he made that statement did he direct you as to what would be acceptable to him? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED

RE: audible alarm

2006-11-16 Thread Craig.Prahl
You can't just wire a flow switch to a bell. You have to have a power source first of all and how would that be supervised in compliance with NFPA 13 or 72? I would ask him to show me the section of NFPA that gives me direction on how to hook it up that way. Craig L. Prahl, CET Fire Protectio

RE: audible alarm

2006-11-16 Thread Craig.Prahl
Ah yes but then couldn't we have the same issue as the AHJ is concerned about, a non-annunciating alarm? If it's not supervised there's no guarantee that it's functional at the time of operation. If I didn't have a fire alarm system I would definitely install a WMA. Also we don't know if th

RE: audible alarm

2006-11-16 Thread Craig.Prahl
Based on the original text, the AHJ wants the flow switch hardwired to the bell. No interconnection between the FS and FACP is mentioned. Based on that concept you could easily have a non-annunciating system that sounded no alarm anywhere. This is his concern with using the FA system for notifica

RE: Interesting article

2006-11-27 Thread Craig.Prahl
I can hear her e-mail box filling up from here. LOL This is just typical. We've had situations like this in our area, not once did any reporter ask about fire protection or sprinklers when the building went BOOM! Most likely they weren't present or weren't operational. But they did ask like 10

RE: Interesting article

2006-11-27 Thread Craig.Prahl
WHAT?! How dare they interrupt the business of Santa for something like a fire alarm! I am shocked and appalled! Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax -

RE: Seismic bracing for CPVC?

2006-12-04 Thread Craig.Prahl
Is your building code seismic analysis stating you need EQ bracing? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg

RE: pump capacity

2006-12-06 Thread Craig.Prahl
Couldn't find anything specifically discouraging us from exceeding 140% except for this: "A.5.8 The performance of the pump when applied at capacities over 140 percent of rated capacity can be adversely affected by the suction conditions. Application of the pump at capacities less than 90 percent o

RE: Casino

2006-12-06 Thread Craig.Prahl
One possibility in the differentiation of classifications between the two is the presence of equipment. In a restaurant you have people seated at tables, not much else there. In a casino there is a lot of electrically operated equipment, extra lighting, more activity. Plus if people lose a lot t

RE: pump capacity

2006-12-06 Thread Craig.Prahl
Sorry, I said supply but meant supply pressure. Something which we are speculating on since it wasn't specifically mentioned anyway. We got off tangent onto two different avenues. Pick, pick, pick, pick ;) Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lo

RE: (no subject)

2006-12-13 Thread Craig.Prahl
Ah yes, the Chinese, best counterfeiters in the world. If you make it, they steal the design and remarket it at less than half your price before you can yell PATENT INFRINGEMENT! ;) I wonder if they copied the UL and FM markings on the deflector as well? But at least they are "springklers" of

RE: Computer equipment

2006-12-14 Thread Craig.Prahl
Composition of computer parts varies by mfgr. You could find anything from ABS to Polystyrene to PVC, but they all fall in the Group A category. One other component of some computer plastics as well as various other electronic equipment are Brominated Flame Retardants - found on printed circuit b

RE: Hanging on bottom of Steel bar joists

2006-12-18 Thread Craig.Prahl
Roof members are generally designed for support of the roof as well as predicted dead load weights for snow, (where applicable) lights, sprinkler piping, and other utilities. It all depends on the facility and what is factored into the design of the roof support system. It's pretty much a given

RE: Hanging on bottom of Steel bar joists

2006-12-18 Thread Craig.Prahl
Dead load is the fixed (non-moving) weight supported by a structural member. Live Load is the weight of items that can move. Dead load is piping or lights, live load is people or fork trucks and such. It is common practice for our structural group to design the roof support system for additional

RE: ESFR in production areas

2006-12-20 Thread Craig.Prahl
In a recent project we had an existing bldg. which had 28ft high double-row racks in a 35ft high bldg. I don't know what they stored on the racks when the bldg. was occupied but anyway, the bldg did have ESFR, K14's in it. Our new client was going to be dividing up the bldg with one half being a

RE: Sprinklers - Chinese Imports

2006-12-20 Thread Craig.Prahl
I doubt that this is the only Chinese company doing this. So vigilance is still necessary. Plus I wouldn't be so willing to trust the word of a company that produces counterfeit products based on pirated technology. I wonder if they even knew what UL stood for when they copied it to their sprink

RE: Sprinklers - Chinese Imports

2006-12-20 Thread Craig.Prahl
Yes I certainly did. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PR

Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
As a contractor I've usually seen sch. 10 grooved piping for anything above 1". But it seems most AE firms are specing sch 40 threaded for anything below 2.5". Now this is for the average project with no special requirements. When I've asked why, there is no real answer other "than that's what w

RE: Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
Matt, does the lower cost of the thrd. Ftgs offset the cost of labor for threading pipe and installation? I wouldn't groove 1", we never did, but 1 1/4" and up we preferred sch. 10 and grooving. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 Intern

RE: Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
Matt, Congrats on finishing up your therapy! LOL Thanks for the input. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www

RE: both QR & SR sprinklers

2006-12-21 Thread Craig.Prahl
George, what in the difference between an SR and QR makes you say that the SR won't provide much "Life Safety"? How much difference in response time can you measure between the two? Quite honestly the smoke detector in the room will be the thing that saves the life of the occupant more so than

RE: Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
Richard the rolled vs. sq. cut has to do with the pipe schedule. Our practice was Sch. 10 is rolled, sch. 40 is cut. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102

RE: both QR & SR sprinklers

2006-12-21 Thread Craig.Prahl
Well I can see that happening in some cases, guess it depends on the type of incident, fuel loading and such. But if the sprinkler goes first at the elevated temperature, that's not much use to the occupant. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Green

RE: Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
Unfortunately in the industrial realm, sprinkler systems are often reluctantly looked upon as a necessary evil. They don't produce any revenue and as far as most clients are concerned they aren't really needed because they've never experienced a fire in any of their other facilities. But they mus

RE: both QR & SR sprinklers

2006-12-21 Thread Craig.Prahl
Chris, I'll take your word for it. (Although I'm a bit disturbed at you and Matt's repeated setting of things on fire.) LOL But I'm sure there are variations in conditions such as flaming fire versus smoldering fires where results may differ. Anyway, I think we've fallen off the original path

RE: both QR & SR sprinklers

2006-12-21 Thread Craig.Prahl
Not trying to disagree with you Bob. I'm sure there are stories which support the importance of each piece of equipment over the other when it comes to saving lives. Just depends on who's telling the story. Both items are important and neither should be discounted in any way. Craig L. Prahl,

RE: Piping installed vs. Piping Spec'd

2006-12-21 Thread Craig.Prahl
Joe I think you missed my intention. (Oh and BTW, I started this topic, so I know what the original question was) If a client wanted or required sch 40, I make sure I knew that before bidding and I would make sure they closely examined all bids to assure that everyone bid apples to apples. I've

RE: hydraulic elevators

2007-01-08 Thread Craig.Prahl
I had been told by one elevator inspector that there was an FM approved hydraulic media that was non-combustible and if that was being used the sprinkler in the pit could be deleted. On the other hand in another jurisdiction I was told that regardless of the hydraulic media used that we were to

RE: hydraulic elevators

2007-01-08 Thread Craig.Prahl
Right on George! It would be better to provide something that some might consider extra then to leave it out since it's in a gray area. That way if you are ever asked if you did all you could have, you can say without reservation, "yes we did". In construction it's all about saving money, an

RE: Another Dumb Article

2007-01-09 Thread Craig.Prahl
High powered sprinkler system? Drowning? Please!!! Ignorance reigns once more!(Sigh.) Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.

RE: max velocity

2007-01-10 Thread Craig.Prahl
Because water faster than 20fps can quickly get out of control and drown people in nursing homes. Slower water is less threatening. But seriously, why place a limit of 20? There are times that through a particular section of pipe where the velocity may exceed that. It makes little sense to have

RE: Testing

2007-01-10 Thread Craig.Prahl
That would most likely depend on the contracting laws of your state or municipality. In our state in order to perform fire sprinkler tests or inspections you have to be a licensed sprinkler contractor. In order to hold that license you have to have a full time NICET level III or IV in Sprinkler L

RE: Testing

2007-01-10 Thread Craig.Prahl
Steve, for an alarm contractor to operate valves without knowledge of what they do would be self-imposing a lot of liability. But as you say, it obviously happens. In our area if an alarm contractor is testing devices attached to or related to the sprinkler system, we were called out to "operate

RE: Testing

2007-01-10 Thread Craig.Prahl
Chris, Kansas isn't alone on that. I have a project in a nearby state. The owner wanted to do the installation himself. He has mechanics that know how to use a pipe wrench. (this guy wanted a detail on his drawings of how to install an upright head, yes we are in trouble...) Anyway, when I

RE: Testing

2007-01-10 Thread Craig.Prahl
Roland, not in our state. An unlicensed owner is limited when it comes to sprinkler installations. He can do small alterations and repairs but not a full blown system install. Not saying that some don't do it all themselves. If no one is looking over their shoulder, who's to know. But you can u

RE: Wood Coating

2007-01-10 Thread Craig.Prahl
If it's not UL listed in the USA, can you legally use it at all? I think it would be difficult to verify any installation against the NFPA 13, 8.14.1.2.10 criteria. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spar

RE: Testing

2007-01-11 Thread Craig.Prahl
John, I believe what you said has merit to a point. I believe that every inspection should entail more than just ringing the bell. Unfortunately that's all a lot of owners want to pay for and that what a lot of inspectors do. It's a fast easy way to make a buck. The inspection should point o

RE: Fire Mains

2007-01-12 Thread Craig.Prahl
Well at least no one drowned. ;) Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- F

RE: Fire Mains

2007-01-12 Thread Craig.Prahl
And this comes back to the question being discussed in another thread, Who approved something like that? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599

RE: max velocity

2007-01-15 Thread Craig.Prahl
Calculated and reality, HUH? Are you not using the actual available flows and pressures? By giving yourself a 10% or 10psi cushion in your calcs you're not creating some mysterious concoction of a system. Not sure what you think is happening. Craig L. Prahl, CET Fire Protection Group Mechanica

RE: max velocity

2007-01-15 Thread Craig.Prahl
Help me out here, while limiting those two items may seem well and good, I fail to see how limiting the pipe velocity to 20fps will extend the life of a sprinkler system. This is not like a plumbing system where water it flowing constantly. In the typical 50 year lifespan of the buildings you kno

Hollywoods version of LH Office Sprinkler Systems

2007-01-17 Thread Craig.Prahl
Sometimes when you've been in the construction/engineering business for a long time it can sure be a detriment to your viewing pleasure. Was watching the movie Changing Lanes, with Ben Affleck and Samuel L. Jackson when what do we come to, oh yeah you can probably guess, the one sprinkler trigger

RE: Sprinkler Save

2007-01-17 Thread Craig.Prahl
Good to hear the sprinklers did their job and it's refreshing to see a well written report of the incident. Someone should get an "attaboy"! Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491

RE: Sidewinders

2007-01-17 Thread Craig.Prahl
These are the ones by Gateway Tubing? We had used them several times on tenant upfit projects. No real issue with them, very quick and easy to install and gave the client some flexibility should future upfits occur. These are only good for lay-in type ceilings so if you have hard ceilings, you ca

RE: POD Storage

2007-01-18 Thread Craig.Prahl
Jim In a perfect world that might be the case but in actuality, the majority of bid projects come with a line on some architectural plan that says "Provide sprinkler protection per NFPA 13 for our highly experimental, top secret, intergalactic, space fuel project" and that's all you get. What yo

RE: POD Storage

2007-01-18 Thread Craig.Prahl
You cannot internally sprinkle the POD units. If you haven't seen them they are for lack of better description, a shipping container. Similar to what you see on ocean going freighters. Those are much larger of course but same basic principal. They are designed to be dropped off at your house an

RE: POD Storage

2007-01-18 Thread Craig.Prahl
One other issue, it depends on which "POD" you are talking about. The brand name "POD" is of a different construction than the so called pod storage units that Home Depot handles. I wonder if POD corporate headquarters would happen to have some fire protection guidelines for warehouses stori

RE: POD Storage

2007-01-18 Thread Craig.Prahl
The biggest problem with interior fire protection of a POD is that you have no assurance that the thing isn't packed wall to wall and floor to ceiling. The sprinkler won't do any good when stuff is jammed up against it. Also, no guarantee that the sprinkler wouldn't get damaged or broke off altog

RE: Exterior Deck

2007-01-26 Thread Craig.Prahl
A project we had a few years ago entailed sprinkling below a deck at a local Sports Bar. The construction was pressure treated wood, ranging from 2ft to about 4.5ft above asphalt pavement. The local Fire Marshal required the sprinklers below because he said that there could be trash accumulation

RE: Exterior Deck

2007-01-26 Thread Craig.Prahl
8.14.6 could definitely be used as a guide and if his deck could meet the criteria of 8.14.6.2 then he wouldn't have to sprinkle. But most decks won't meet #3 in that list since decking boards can be 1/8th inch or more apart, the AHJ may not consider that "tight construction". Craig L. Prahl,

RE: Non-Combustible Crawl Space

2007-01-26 Thread Craig.Prahl
It sounds like NFPA 13 (2002) 8.14.1.2.2 could apply to your situation. If that's true then no sprinklers would be required. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4

RE: sprinkler accident sets off Seattle electrical fire

2007-01-29 Thread Craig.Prahl
Sounds like an angry tenant beating the daylights out of a sprinkler with a broom handle. "Yeah I was uh, like uh, cleaning, yeah that's what I was doing officer". But agreed, discharge from ONE or TWO sprinklers traveling 20+ floors and FLOODING the building? I'm just glad no one drowned bec

RE: FIRE PUMP ROOM ACCESSIBILITY

2007-01-30 Thread Craig.Prahl
If you have to turn sideways to get into the room, a firefighter in full turnout gear won't be able to get in. If you have a local fire marshal that reviews and approves installations the owner might be in for a big surprise if he rejects the installation just before they expect to occupy the faci

RE: Floating Ceilings

2008-08-05 Thread Craig.Prahl
The presence of a return air plenum doesn't automatically necessitate sprinklers. Sprinklers are going to be required in the space if combustibles with ratings equal to or above that which is allowed for a concealed space are present as defined in NFPA 13. If it is a plenum it may actually be

RE: Floating Ceilings

2008-08-05 Thread Craig.Prahl
There's the issue, the ceiling in question wouldn't be considered a floating cloud, (my point), with just small openings for return air. I envision the floating clouds as those panels scattered throughout an area intended for acoustic absorption or architectural flavor but not necessarily atta

RE: Floating Ceilings

2008-08-05 Thread Craig.Prahl
So would it be "almost protected". lol And let's not go any farther with the "qualifications" thing. Time for a new topic... Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Di

RE: New topic

2008-08-05 Thread Craig.Prahl
You need to provide a bit more info. When dealing with storage occupancies you need to clarify what is being stored, how it's being stored (racks, shelves, bins, on floor, pallets), in what type of container (box, crate, tote, jars, etc.), encapsulated, heights of said commodities, etc. Once y

RE: New topic

2008-08-05 Thread Craig.Prahl
And that's where it's going to be because if it's just ceiling sprinkler coverage, OH is OH and EH is EH regardless of the occupancy. So there's no reason to repeat the info specifically in the storage section of 13 when the limitations of the specific sprinkler type and spacing is listed elsew

RE: New topic

2008-08-06 Thread Craig.Prahl
If he's unsettled over the issue I'd tell him that since 231 and 231C were incorporated into 13, then all the related information of 13 now becomes intertwined with what used to be in those other documents. There's not much more you can do. Craig L. Prahl, CET Fire Protection Group Mechanical

RE: Backflows

2008-08-06 Thread Craig.Prahl
What are you trying to protect from what? Not sure what kind of pieces are going to be burped up by the BFP? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax

RE: Backflows

2008-08-06 Thread Craig.Prahl
The location of those are often dictated by the Water Department. Have they offered any opinion or requirement? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax -

RE: indoor suction tanks

2008-08-06 Thread Craig.Prahl
Have you considered a depressed slab/sump with a vertical turbine pump arrangement instead of tanks? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439

RE: Mattress stroage

2008-08-07 Thread Craig.Prahl
Interesting since NFPA 13 A.5.6.3 (2007) lists foam mattresses (in finished form) as a Group A Plastic. Box springs which are mostly wood and metal as Class III. I would consider the foam in the sofas and probably lean toward classifying them the same as the mattresses. They probably looked a

RE: Mattress stroage

2008-08-07 Thread Craig.Prahl
I hope he specified more than just ESFR. Did he give you any specifics or has he left the selection of pressure and K-factor up to you? Depending on the water data and what is chosen you may or may not need a pump. Hopefully he gave you recent water information so you don't have to guess. ESF

RE: Mattress storage

2008-08-07 Thread Craig.Prahl
If you read the definition of expanded and exposed you could say that a foam mattress with the cloth coverings MAY be considered as being Exposed. (definition of exposed in 3.9.1.10, 2007) since the cloth covering could absorb water... BUT the addition of the plastic bagging of the items takes

RE: Soleniod valve

2008-08-11 Thread Craig.Prahl
Oh this scenario gets sooo old. With the recent discussions concerning the response time of certain types of smoke detectors it is very likely that the valve would never be actuated in time for the sprinklers to do anything. Is he willing to take that risk? Can the valve be supervised by

RE: Soleniod valve

2008-08-11 Thread Craig.Prahl
Oops, sorry, my mistake. I forget. lol Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original Messa

RE: "green" dry chemical agent

2008-08-13 Thread Craig.Prahl
I think Tyco's version is called Sapphire, same thing just different name basically. But it's not a dry chemical, it's a highly atomized, non-conductive, liquid, discharged at very high pressure. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 Int

RE: FM-200 Decomposition Product _URGENT!!!

2008-08-13 Thread Craig.Prahl
Chances are his reaction was more due to toxic gases and smoke released from the burning material than from the FM-200. Remember furniture can have foam plastics, and other materials that release several different toxic gases from the burning process. I wouldn't walk into a fire scenario witho

RE: "green" dry chemical agent

2008-08-13 Thread Craig.Prahl
Is that a water mist system? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [

RE: Viking H-1

2008-08-18 Thread Craig.Prahl
headed your way via e-mail Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [EM

RE: underground through building

2008-08-18 Thread Craig.Prahl
You've got a bunch of issues there. Pipe under buildings: check NFPA 24, 10.6.1 PIPE SHALL NOT BE RUN UNDER BUILDINGS. There is some allowance when it can't be avoided as listed in 10.6.2. Can the pump room be accessed directly from outside? Is there any way to service or even remove the pu

RE: foward flow test

2008-08-18 Thread Craig.Prahl
The requirement of a backflow assembly depends on your water supply connection. If you are getting your water from a municipal supply then you will have one, (as opposed to drawing your fire water from a private fire water storage tank). Any AWWA approved assembly is what is being referenced.

RE: Xerxes tank suction line

2008-08-25 Thread Craig.Prahl
Well you know how it goes, what may be acceptable to one AHJ may not be to another. But regardless, their acceptance still doesn't make it compliant with code. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartan

RE: Computer room Racks with Blade Servers

2008-08-26 Thread Craig.Prahl
We had similar discussions with a client on a very large automotive project. The Underwriter was directing them to provide automatic sprinklers in the data center control rooms, they wanted nothing or at best FM-200 alone. The Underwriter had discussed business interruption with them and aske

RE: Computer room Racks with Blade Servers

2008-08-26 Thread Craig.Prahl
What is the AHJ's definition of this space? Is it a room or an equipment enclosure? If it's an equipment enclosure, then the min. door hgt. would have no bearing. You also then have to look at the requirement of sprinklers within an equipment enclosure versus in an occupied room. Crai

RE: anybody out there?

2008-08-26 Thread Craig.Prahl
we're all at the beach on vacation, sorry. catch ya when we get back.. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED]

RE: Re[2]: anybody out there?

2008-08-26 Thread Craig.Prahl
Sorry, what can I say? ;) Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [

RE: Computer room Racks with Blade Servers

2008-08-26 Thread Craig.Prahl
I've done some queries but haven't got much to go on. Basically due to tight controls there are few news worthy computer/control room fires. Those that do occur usually don't make the news just because they aren't all that dramatic. http://www.highspringsherald.com/articles/2007/03/01/news/news

RE: FM-200 enclosure volume (Exclude Cabinets volume?)

2008-09-03 Thread Craig.Prahl
Why would people still be in the room while the FM-200 is being discharged? There will be alarm notifications before this occurs to warn them of the discharge, they should be vacating the room. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 Int

RE: FM-200 enclosure volume (Exclude Cabinets volume?)

2008-09-03 Thread Craig.Prahl
If in fact it is a requirement by the employer/owner that personnel remain in the room when a system discharges someone needs their head examined. If the system is in discharge mode it is likely there is a fire scenario occurring, what imbecile would require his employees to "go down with the sh

RE: Protection of Group 3 Aircraft Hangars

2008-09-03 Thread Craig.Prahl
What type of storage does NFPA 101 not require to be sprinkled? The building code requires sprinklers for some depending on the commodity stored. How can an aircraft be considered a low hazard commodity? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1

RE: Origin & Intent of 10 psig Minimum Suction Pressure for Boosters

2008-09-09 Thread Craig.Prahl
Ask them to give you a copy of the referenced section. You shouldn't have to go on the hunt. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL

RE: Low Expansion Foam System

2008-09-10 Thread Craig.Prahl
An NFPA 16 foam water system would be a better choice than low expansion foam. Check NFPA 30, 16.4 and then go to NFPA 16. Per NFPA 30, in rack sprinklers for foam-water systems are installed per NFPA 13 criteria. Low expansion foam won't help you when it comes to racks. Check NFPA 11 for low

RE: Help!! Sprinkler in Planetarium

2008-09-10 Thread Craig.Prahl
It would seem out of place for the fire department or AHJ to take design authority over a project unless they are willing to stamp drawings and be totally responsible for that design. It would be appropriate for them to make suggestions and recommendations like an Underwriter would but not perf

RE: Coal Bunkers

2008-09-11 Thread Craig.Prahl
NFPA 85 has a lot of verbiage concerning coal bunkers. But there's not a lot if any fixed fire protection involved. Prevention and suppression is mostly controlled by various procedures and operational methodology. Check it out. Also might look at NFPA 120, FMDS 6-24(Coal Pulverizers and Pulv

RE: Paint booths - explosion proof tamper switch

2008-09-16 Thread Craig.Prahl
Yup, part of the electrical code. See Article 505 to start for descriptions of classified areas. If the hazard present warrants, the electrical devices and components must be rated. Somewhere along the project the electrical engineers will do a hazardous location plan and identify the areas w

RE: Paint booths - explosion proof tamper switch

2008-09-16 Thread Craig.Prahl
Here's a pic from NFPA 70, 516. 3 foot bubble outside the doors as has been described. [cid:873540416@16092008-0B36] Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102

RE: Vertical Shafts

2008-09-19 Thread Craig.Prahl
8.15.2 says if they are non-combustible or limited combustible, non-accessible that they don't require sprinklers. Where the confusion in that? Hopefully they are non-accessible otherwise you'd have prisoners up in the attic, right? When you say shaft, what it the purpose of the shaft? How b

RE: Solarium

2008-09-22 Thread Craig.Prahl
Does he reference a particular code requirement? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original

RE: Solarium

2008-09-22 Thread Craig.Prahl
Look at NFPA 13, 2007, 8.5.7, he may be looking at this as if it is a ceiling pocket. But in any case I couldn't find reference to a skylight smoke detector requirement unless it's being used for smoke control. The following excerpt is from the IBC, 2006 limiting the allowable area but also gi

RE: mist sprinklers protecting computer rooms

2008-09-23 Thread Craig.Prahl
This one of those situations where people don't think the whole process all the way through. VESDA is a great system, very expensive and quite often overkill unless you have a critical operation with a lot of sensitive data and no backup. (High Value data centers should ALWAYS have a backup sy

RE: Dry Valve Keeps Tripping

2008-09-25 Thread Craig.Prahl
Ok, need some help here, if the accelerator trips doesn't that usually mean there is an open pipe in the system usually indicating a leak or open head? The accelerator is there to aid in quicker dissipation of air in the system to allow the dry valve to open within the required time period. I

RE: Dry Valve Keeps Tripping

2008-09-25 Thread Craig.Prahl
Thanks, Based on the detailed description it sounds like the accelerator alone can not trip the valve. That actuation has to be a result of loss of air pressure in the system as said before. The loss of system pressure will allow the accelerator to do it's job which is to decrease the amount

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
The Tyco head is specifically listed to provide protection equivalent to a two hour rated assembly. So if the corridor is a rated exit corridor then you need to use the Tyco head to maintain the integrity of the separation. There is no equivalent rating for sprinklering a window with just an a

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
Be careful, if the AHJ approves something that is an incorrect application as you suggest, you share responsible for the incorrect application too, not just him. Make sure that what you choose meets code and is correct for the particular situation. Can you defend your installation or design be