[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Larry Keeping
FYI, if it is a retrofit, you are not specifically tied to 12.6.2 and 12.6.3 
with sprinklers of K-11.2 or greater. The following Subsection 12.6.4 is an 
"exception" to those provisions:

12.6.4*   Unless the requirements of 12.6.5 are met, the requirements of 12.6.2 
and 12.6.3 shall not apply to modifications to existing storage application 
systems, using sprinklers with K-factors of K-8.0 (115) or less.

A.12.6.4   Modification of an existing system includes extending sprinkler 
protection into adjacent areas.

With this, EOR call ups not-with-standing, NFPA 13-2013 allows you to utilize 
any K sprinkler that works for you hydraulically.

The foregoing is my opinion only and does not represent NFPA or the NFPA 13 
Technical Committees.

Best regards,

Larry Keeping

From: Brian Harris 
Sent: Monday, September 11, 2023 1:46 PM
To: Discussion list on issues relating to automatic fire sprinklers 

Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Warning! This email came from outside your company.
Travis-
Thanks. I should have mentioned I need it to be an upright. It's a retro-fit 
job.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Travis Mack mailto:t.m...@mepcad.com>>
Sent: Monday, September 11, 2023 1:40 PM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

https://www.reliablesprinkler.com/files/bulletins/146.pdf?x76626


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: t.m...@mepcad.com<mailto:t.m...@mepcad.com>

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Brian Harris mailto:bhar...@bvssystemsinc.com>>
Sent: Monday, September 11, 2023 10:34 AM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Eric-
Thank you. I have an EOR that called for a K14.0 CMDA on a specific job. Since 
I can't find one, I was wondering if I could use a K11.2 instead.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Eric Rieve mailto:e...@rievefire.com>>
Sent: Monday, September 11, 2023 11:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

To expand on this slightly, it's not that "general storage applications" 
directly means class I-IV commodities, but that chapter 12 applies to all the 
following storage criteria chapters. So, "general storage applications" is how 
they show that 12.6.3 applies to chapters 14 and 15 for solid-piled 
commodities, and then "rack storage" is there to reference chapters 16 and 17. 
The rest of the sentence containing "rubber tire storage, roll paper storage, 
and baled cotton storage" is how they reference chapters 18, 19, and 20 
respectively to round out the rest of chapters.

[A close up of text]

Hope this helps!

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris mailto:bhar...@bvssystemsinc.com>>
Sent: Monday, September 11, 2023 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Eric-
Thank you. I didn't want to assume class I-IV fit into "general". Much 
appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f=E,1,0GPrjmr1UnUZUD1dC2S_0zPb18z5RsmivEapMbxWxXZh0Z8xeW_wo38ttJ26ezgjT88xjZeUN-zIwYtZW3LVrX02vu1_1ePrf-JdHuJVtMUmNiCMD84,=1>


From: Eric Rieve mailto:e...@rievefire.com>>
Sent: Monday, September 11, 2023 11:27 AM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

Yes, it does per the "general storage applications" segment of the code section.

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris mailto:bhar...@bvssystemsinc.com>>
Sent: Monday, September 11, 2023 11:19 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] CLASS I-IV / CMDA

Would 12.6.3 (NFPA-13 2013) apply for class I-IV? My remote area is .36/2000.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f=E,1,Fz_3mU2H_Ojb1YY6oijGOLnnNaRa7hDR_0xsbgsJ7z6pCBxHT1MEGLQdRZPurT2UN0kMjjHnC-ulMsxAg9BZ1lIW3A4QFGpu82oXRLmyd4G-kzjUnLn2Yg,,=1>
Phone: 704.896.9989
Fax: 704.896.1935




RE: pipe schedule/residual pressure

2021-06-04 Thread Larry Keeping via Sprinklerforum
I'm not sure how the wording got revised over the years, but back-in-the day 
the standard was a lot clearer that the residual pressure was measured at the 
base of the riser. Here is what the old note used to say under the table for 
Water Supply Requirements for Pipe Schedule Sprinkler Systems:

NOTES:
1. The pressure required at the base of the sprinkler riser(s) shall be 
the residual pressure required under the roof plus the  pressure required to 
reach this elevation.

Whenever I've done such evaluations, the analysis would take into account the 
losses due to elevation and friction losses in the underground piping, between 
the water supply at the street and the base of the riser, based on flowing the 
Acceptable Flow at Base of Riser (Including Hose Stream Allowance) from the 
table.

Then I would factor in the loss through the backflow preventer and the pressure 
due to the elevation to the highest sprinkler. Thus determining the residual 
pressure under the roof.

Since the evaluation is for existing systems, the Minimum Residual Pressure 
Required only needs to be the 15 psi for light hazard  or the 20 psi for 
ordinary hazard.  The 50 psi value is only for new systems thar are greater 
than 5000 sq.ft.  For the new system, I would usually opt to calculate  it 
hydraulically.

It should be recognized that the above is my personal opinion and not that as a 
member of the NFPA and should therefore not be considered, nor relied upon, as 
the official position of the the NFPA, nor any of their technical committees.

Best regards,

Larry Keeping. P.Eng.
Senior Technical Specialist

PLC FIRE SAFETY SOLUTIONS
3413 Wolfedale Road, Suite 7
Mississauga, ON L5C 1V8

Phone:   905-949-2755 Ext 204
Fax:    905-949-1752
Email:     lkeep...@plcfire.com
Website:    www.plcfire.com
Toll Free:   1-800-675-2755



-Original Message-
From: Sprinklerforum  On Behalf 
Of Jamie Seidl via Sprinklerforum
Sent: June 4, 2021 4:14 PM
To: Sprinklerforum 
Cc: Jamie Seidl 
Subject: pipe schedule/residual pressure

Warning! This email came from outside your company.

I am looking at a project where we are renovating an existing building with a 
new system.  There are other buildings on the site (1930's vintage) that share 
the underground lines.  To bring the site into compliance with current codes, 
RPZ backflows are being added at the entrance to the site.
The existing buildings are occupied, and the fire department is looking for 
some assurance that the systems will work with the addition of the backflow 
preventer.  I remembered (though have never applied it) section 11.2.2.8 allows 
for the calculation of the residual pressure at the highest sprinkler, and 
deducting elevation, BFP losses ect...  The buildings in question are over 5000 
sqft, so the minimum 50 psi will apply.
So my question is, do I just utilize the residual pressure from the closest 
hydrant, deduct the elevation and backflow losses from the residual and call it 
a day?  Or do I need to account for additional friction through the system 
piping?  Both 13 and the handbook seem to be mute on this.
Thanks again, Forumites.
Jamie  Seidl
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Interstitial Space

2021-05-11 Thread Larry Keeping via Sprinklerforum
Way back-in-the-day, when NFPA 13 would fit in a back pocket, there was a 
Formal Interpretation 80-29(A) that addressed interstitial spaces.
It remained in play until at least the 1999 edition, there is a copy in the '99 
Handbook. I never saw it "withdrawn", but it was probably dropped from 
reference when NFPA 13 added text for concealed spaces not requiring sprinkler 
protection, because it doesn't seem to be in the '02 Handbook.

Anyway, here is what that old FI said in the '99 Handbook:

Formal Interpretation 80-29(A)

Reference 5-1.1, 5-13.1.3

Background:   Construction - Structural steel frame with concrete floors. The 
floor-to-floor height is approximately 15½ feet. Approximately 9 feet above 
each floor, a gypsum deck has been poured to form an "interstitial space." 
Non-combustible ductwork, plumbing, electrical conduit, sprinkler piping and 
open cable trays run in the interstitial space. Access to the space is by five 
stairways, with access doors each being approximately 3 feet by 3 feet.

Question:   Is it the intent of 5-1.1 of NFPA 13 that sprinkler protection of 
the interstitial space described above be provided to consider the building 
completely protected by automatic sprinklers?

Answer:  No.   The space described is essentially non-combustible with no 
occupancy and no combustible services [with the possible exception of the cable 
trays which could be protected in accordance with 5-5.1.3 if necessary] and so 
could be treated as a non-combustible concealed space. Use of the space for 
storage or the introduction of combustibles would require provision of 
sprinklers to maintain classification as completely protected by automatic 
sprinklers.

Issue Edition:   1980

Reference:   3-10.3, 4.1

Date:   October 1982

Please note there is a typo in that FI, because there is no 5-5.1.3 in NFPA 
13-1999, and 5-13.1.3 does not seem to be applicable either.
I think that reference in the answer should have been to 5-13.1.4 (b), which is 
the text that was referenced (as 4.4.4.4 (b)) in previous Handbooks in my 
library.

I hope that you find this helpful,

Larry Keeping


-Original Message-
From: Sprinklerforum  On Behalf 
Of Ken Wagoner via Sprinklerforum
Sent: May 11, 2021 3:51 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ken Wagoner ; Mike Hairfield 
Subject: Re: Interstitial Space

Warning! This email came from outside your company.

Mike,

I'm not sure which edition of the standard governs this project, however:
from the 2016:
8.15.1.2.1 concealed spaces of non- or limited combustible construction require 
no sprinklers
8.15.1.2.2 concealed spaces of non- or limited combustible construction with 
limited access, and no occupancy, or storage of combustibles require no 
sprinklers.

Those same sections are unmodified in the '19 edition, in 9.2.1.1 and 9.2.1.2.

hope that helps,
*Ken Wagoner, SET
*Parsley Consulting*
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> *


**
On 5/11/2021 12:38 PM, Mike Hairfield via Sprinklerforum wrote:
> Got a project where there is a walkable ceiling with a non-combustible 
> interstitial space above.
>
> FM Global did not require sprinkler protection in this space.
>
> The local AHJ is saying that it needs to be protected with sprinklers.
>
> Where in NFPA-13 can I find where it doesn't require protection.
>
> Thanks,
>
> Mike
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Soybean, corn, oat, & wheat storage

2021-04-07 Thread Larry Keeping via Sprinklerforum
>From NFPA 13-2016, Table A.5.6.3:

Food Products - Non-Frozen

Dry foods (such as baked goods, candy, cereals, cheese, chocolate, 
cocoa, coffee, grains, granular sugar,  nuts, etc.); bagged  or cartoned
Class III

Larry Keeping

-Original Message-
From: Sprinklerforum  On Behalf 
Of Jamie Seidl via Sprinklerforum
Sent: April 7, 2021 3:38 PM
To: Sprinklerforum 
Cc: Jamie Seidl 
Subject: Soybean, corn, oat, & wheat storage

Warning! This email came from outside your company.

I am looking at a project that is storing soybean, corn, oat and wheat seeds in 
large polypropylene  bags (think large sand / rock bags) . The client has 
indicated that these are to be stored on floor, two high for a total storage 
height of less than 12'.  I know NFPA 13 does not address this, and FM seems to 
be silent also.
Based on the storage height, and free flowing nature of the product I am 
leaning towards an ordinary group 2 classification, but wanted to run it by the 
forumites to see if anyone has run across this in the past.
Any Takers?

Thanks,
Jamie Seidl
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Check Valve After Flow switch?

2021-03-17 Thread Larry Keeping via Sprinklerforum
A while back I questioned a contractor's installation that didn't follow the 
Potter guidelines, so the contractor got a letter from Potter.

This letter said:

"...   This is only a recommendation, not a requirement.   ..."

"...   There are no UL, FM, or NFPA codes or standards requiring a 
certain distance between a valve or fitting and a flow   switch. If the 
device passes the flow test it can be considered an acceptable installation.   
..."

"...   We simply may have overcome the need to maintain this distance 
recommendation as our product has evolved and improved over the years."

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum  On Behalf 
Of Matthew J Willis via Sprinklerforum
Sent: March 15, 2021 7:40 PM
To: sprinklerforum@lists.firesprinkler.org; Mike Henke 
Cc: Matthew J Willis ; Steve Leyton 

Subject: Re: Check Valve After Flow switch?

Warning! This email came from outside your company.

Yeah, I get the listed assembly.

Just begs the question,
If it's good for the goose..

I know jurisdictions that reject if you do not have the 3psi loss on your calcs.

Sure they have a listing, but there are folks out there that think only a 
listed can be installed.
When in reality, listed devices need only need installed.

Matt

Get Outlook for Android<https://aka.ms/AAb9ysg>


From: Mike Henke 
Sent: Monday, March 15, 2021 5:35:13 PM
To: sprinklerforum@lists.firesprinkler.org 

Cc: Steve Leyton ; Matthew J Willis 

Subject: RE: Check Valve After Flow switch?

Steve is correct. The flowswitches on the listed preassembled manifolds and 
risers are part of a listed assembly and are tested as part of that assembly.
The recommendations on the Potter literature are recommendations, not code 
requirements. The purpose of the recommendation is to try to prevent people 
from installing the flowswitch too close to a valve or change in direction that 
could cause enough turbulence to prevent the flowswitch from operating when a 
calibrated flow test is conducted. The installer would then have to relocate 
the flowswitch.

Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___



Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com   |   www.pottersignal.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Monday, March 15, 2021 6:26 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; Matthew J Willis 

Subject: RE: Check Valve After Flow switch?

If an assembly is tested and listed as a unit, and passes the required tests as 
configured, then the listing supersedes such restrictions.   I remember asking 
this question when Resi-Risers first came out.

Steve L.

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matthew J Willis via Sprinklerforum
Sent: Monday, March 15, 2021 3:45 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis 
Subject: RE: Check Valve After Flow switch?

I would as well.

What happened to the "not within 24" of a drain or valve?"

A check valve is a valve.. Right?

R/
Matt

-Original Message-
From: Sprinklerforum  On Behalf 
Of John Denhardt via Sprinklerforum
Sent: Monday, March 15, 2021 3:36 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Denhardt 
Subject: Re: Check Valve After Flow switch?

I would like to know why this is the "best way" for the installation.  I am not 
stating it is not, just not sure why one way is better especially since we have 
done it a certain way for years.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Expand your business with ITM*
Professionalize the role of your inspection team with AFSA’s ITM Inspector 
Development Program. This comprehensive 20-month program provides a blended 
learning environment teamed with robust curriculum created by top industry 
leaders. Plus, the first six-months of instruction is online. Now enrolling for 
Spring 2021 <https://www.firesprinkler.org/itm>.




On Mon, Mar 15, 2021 at 5:05 PM Henry Fontana via Sprinklerforum < 
sprinklerforum@lists.firesprinkler.org> wrote:

> Hello all.
>
> This is not a code change. Both manufacturers (one of them I work for) 
> state that this is the best way for in

RE: Tyco LFP - antifreeze

2021-02-10 Thread Larry Keeping via Sprinklerforum
I beg to differ. 

I  was looking into using the new TYCO A/F on one of my projects, but when I 
met with one of their reps. I was advised that the listing is  for system 
volumes of 50 US gallons or less.

Best regards,

Larry

Larry Keeping. P.Eng.
Senior Technical Specialist

PLC FIRE SAFETY SOLUTIONS
3413 Wolfedale Road, Suite 7
Mississauga, ON L5C 1V8

Phone:   905-949-2755 Ext 204
Fax:    905-949-1752
Email:     lkeep...@plcfire.com
Website:    www.plcfire.com
Toll Free:   1-800-675-2755

DISCLAIMER:  This email and any files transmitted with it are confidential and 
intended solely for the use of the individual or entity to whom they are 
addressed. If you have received this email in error please notify the sender, 
delete this e-mail and destroy any copies. Any dissemination or use of this 
information by a person other than the intended recipient is unauthorized and 
may be illegal. The recipient should also check this email and any attachments 
for the presence of viruses. The company accepts no liability for any damage 
caused by any virus transmitted by this email. E-mail transmission cannot be 
guaranteed to be secure or error-free as information could be intercepted, 
corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The 
sender therefore does not accept liability for any errors or omissions in the 
contents of this message, which arise as a result of e-mail transmission.
 
 Please consider the environment before printing this email.



-Original Message-
From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: February 10, 2021 10:22 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: RE: Tyco LFP - antifreeze

Warning! This email came from outside your company.

Interesting stuff with the AF.  It is good for up to 500 gal system capacity.  
However, if you are over 200 gallons, you must calculate as a dry system.  That 
seems to negate the use of AF over 200 gallon capacity.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
mailto:travis.m...@mfpdesign.com
www.mfpdesign.com

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0

From: Sprinklerforum  On Behalf 
Of David Williams via Sprinklerforum
Sent: Wednesday, February 10, 2021 8:19 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: David Williams 
Subject: Tyco LFP - antifreeze

Hey Scott and other cold weather practitioners in Fire Protection. Any feed 
back on the "new" Tyco LFP antifreeze. Looks like it may have some use in 
southern MN locations, but with Duluth at annual 99% extreme of -24.9 and 50 
year extreme at -36.6 maybe not such a good idea yet. We plan on sticking with 
the dry systems we have been specifying since the flammability concerns about 
glycol came out unless working south of Minneapolis!

As per Scott we spec nitrogen for dry systems, but it sure seems owners want to 
take the VE from the sprinkler contractors even when we present the long term 
value to them.

David Toshio Williams, PE*, FPE - Lead MEP/FP Engineer (*Registered in MN, WI, 
MI, IA, IL, IN, ND, VT)
21 West Superior Street, Suite 500, Duluth, MN 55802 Direct 218.279.2436 | Cell 
218.310.2446 LHBcorp.com LHB, Inc. | PERFORMANCE DRIVEN DESIGN.

...sent from the cloud through the tubes!
___
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Distilled Spirits

2021-02-03 Thread Larry Keeping via Sprinklerforum
Here is something from the March/April 2018 NFPA Fire Journal:

"NFPA codes and standards and other codes like the International Fire Code 
(IFC) don't include information specifically about distilling-a result of the 
industry's history of lobbying and self-regulation. Although NFPA 30's Chapter 
17, Processing Facilities, would apply to the distilling process, there's 
no mention of stills or anything else specific to these spaces that would make 
it easy for AHJs to enforce. The code excludes spirits from its chapters on 
storage. "[AHJs] need  something more in a code to help them know what to look 
for and what hazards are being presented," Gittleman says.

The DISCUS fire protection manual, a product of input from large distillers 
like Jim Beam, provides a lot of this information in a relatively 
easy-to-digest manner. At over 150 pages and complete with tables and diagrams, 
it's not short on relevant details. It references numerous NFPA codes 
and standards ...".

I had a copy of the DISCUS Manual way-back-when, and it was great.

Also, I believe FM has a data sheet on alcohol /barrel storage.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum  On Behalf 
Of Matt Grise via Sprinklerforum
Sent: February 3, 2021 1:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise 
Subject: RE: Distilled Spirits

Warning! This email came from outside your company.

The production area (distillery) is listed in the 13 annex as OH2. The storage 
would probably be NFPA 30.

Matt


-Original Message-
From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, February 03, 2021 12:25 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com; trilliumf...@cwisp.ca
Subject: RE: Distilled Spirits

If you are over 20% alcohol, I believe you go into flammable liquids stuff. Try 
over in that direction.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271 ext. 700 C: 480-272-2471
mailto:travis.m...@mfpdesign.com
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.mfpdesign.com=E,1,OWMzZSRhKB4XqBaXs-PlCGH6HcuM6Ok_Q5bhLJVaaA28325NKVd28IqxTiQZ3a7TpNkIc7RNsSlyeSsUDFKCSXM3PZlBnhjZ7Aw23QjecC7Rpi8RFDWXvwRBhmo,=1

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0

From: Sprinklerforum  On Behalf 
Of Trillium Fire Sprinkler Design Inc. via Sprinklerforum
Sent: Wednesday, February 3, 2021 11:21 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Trillium Fire Sprinkler Design Inc. 
Subject: Distilled Spirits

Can anyone direct me to design criteria for the manufacturing and storage of 
distilled spirits ( Rum)?



Any info would be greatly appreciated.



Thank you



Troy

___
Sprinklerforum mailing list
mailto:Sprinklerforum@lists.firesprinkler.org
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org=E,1,Em7J0PeoiwFnWUKftG9NGBT6Gf9_ZW6_YjrI8pq-jlRyZUO6UlxtpNQUdey-ogrxKS3qPoy90Ad_7_uJqP6QLfiZUdO3aG-QfQjO9s288GU,=1

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org=E,1,OFxEpnsL7-F1epzxBqoITLrv1x2gmS1P8eNzedF-nx9ttDqrqw4GZNpIaoDFklyM6SgFZuE6A2qBOtk-aXch6KGSwgXWHUKJvXO8mjyLyvQ75RE,=1
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: schedule 7 pipe?

2021-01-21 Thread Larry Keeping via Sprinklerforum
Good morning:

I have been reading through this e-mail chain and I noticed a couple of 
references to the ASTM A-53 pipe spec. 
I stand to be corrected, but out that in all of the data sheets that I have 
ever seen, for "Schedule 7" or for any other listed sprinkler pipes, with wall 
thicknesses less than Schedule 40, are to the ASTM A135/A795 specs.
The only data sheets that I am familiar with that meet the ASTM A53 spec. is 
for Schedule 40 pipe.

Larry Keeping

-Original Message-
From: Sprinklerforum  On Behalf 
Of John Denhardt via Sprinklerforum
Sent: January 20, 2021 5:13 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Denhardt 
Subject: Re: schedule 7 pipe?

Warning! This email came from outside your company.

Matt - fully understand the position you have.

To answer your initial question specifically, I have heard of *no* push to 
change NFPA 13 with regard to piping material.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*


*Expand your design department in 2021!* AFSA is taking its popular two-week 
Beginning Fire Sprinkler System Planning School on the road. From San Diego to 
Tampa Bay and stops in between, our technical experts will teach the basics of 
system layout based on the 2019 edition of NFPA 13. Space is limited. Enroll 
today at https://www.firesprinkler.org/schools.


On Wed, Jan 20, 2021 at 5:03 PM Matt Grise via Sprinklerforum < 
sprinklerforum@lists.firesprinkler.org> wrote:

> There is no doubt  that thicker pipe lasts longer.
>
> However, when the owner of a warehouse specifies schedule 7 piping for 
> the sprinkler system in a hard bid, the installing contractor will be 
> using schedule 7.
>
> Matt
>
> -Original Message-
> From: Lucas Kirn 
> Sent: Wednesday, January 20, 2021 3:34 PM
> To: Matt Grise ; 
> sprinklerforum@lists.firesprinkler.org
> Subject: RE: schedule 7 pipe?
>
> Matt,
>
> Having seen many cases of failed sch. 7 pipe over the past 10+ years I 
> would tell anyone willing to listen to stay far, far away from it. 
> Pipe schedule is the most basic form of corrosion/leak protection. The 
> thinner the pipe, the shorter the lifespan.
>
> I have also seen several instances where a GC or property owner came 
> back and tried to sue the installing sprinkler contractor because the 
> system started leaking after less than 10 years - through no fault of 
> the contractor. In my opinion installing an inferior product exposes 
> your company to more liability.
>
> Lucas Kirn, PE
>
> Engineered Corrosion Solutions
> (314) 415-1387 |
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fecscorrosion.com=
> E,1,xpOWPXSiPcfMjrQXW0481anSuS-LAdKXY8Csy9gBfPzMFPZQ61fHBTnx1JPCTU5vcU
> quYUcmx0Hs_Eg8_66rAgyi9fc2BhzVgD_0ACnhMOXX6-GkecLttgY,=1
>
> -Original Message-
> From: Matt Grise 
> Sent: Wednesday, January 20, 2021 9:58 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: schedule 7 pipe?
>
> Has there been any push/interest in allowing unlisted (standard ASTM 
> A53) schedule 7 steel pipe to be allowed by code in place of the listed "flow"
> piping options?
>
> Matt
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 3000 sqft rule

2020-03-04 Thread Larry Keeping via Sprinklerforum
According to my records, there has been a “3000 sq. ft. rule” as long as there 
have been area / density curves.

In the 1973 and 1974 editions, there was a note below Table 2-2.1(B) that said:

   For combustible construction with wet or dry system the minimum 
area of application shall be 3,000 sq. ft.

Then for the 1975 edition the note was modified to say:

For construction having unsprinklered combustible concealed spaces, the 
minimum area of sprinkler operation shall be 3,000 square feet.

Best regards,

Larry Keeping



From: Sprinklerforum  On Behalf 
Of Ron Greenman via Sprinklerforum
Sent: March 4, 2020 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ron Greenman 
Subject: 3000 sqft rule

Does anyone know what edition of 13 the 3000 sqft rule was introduced?


Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Missing table in chapter 21

2019-12-06 Thread Larry Keeping via Sprinklerforum
I think you meant to ask what happened to Table 21.2.2.

During the revision cycle for the 2016 edition, Section 21.2 was greatly 
revised. Table 21.1 was deleted and so Table 21.2.2 from the 2013 edition 
became a new Table 21.2.1 in the 2016. This table was also revised, to delete 
the bin box and shelf storage, hose stream and duration columns, etc. so it 
looks different. Here is the Committee Statement for First Revision No. 229:

“The revisions to section 21.2 and the associated tables eliminate a 
significant amount of redundancy. Hose stream and duration columns were deleted 
since this required is address in Table 21.4.1. Extended coverage sprinklers 
utilizing Fast Response or Standard Response elements are all in the standard 
response category. The testing associated with the referenced sprinkler did not 
include bin box or shelf storage, therefore these arrangements are not 
considered in the tables.”

In the 2019 edition, it is now Table 24.2.1.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Ben Young via Sprinklerforum
Sent: December-06-19 3:48 PM
To: 321 via Sprinklerforum 
Cc: Ben Young 
Subject: Missing table in chapter 21

Does anyone know what happened to Table 22.2.2 in between the 2013 and 2016 
editions?
Nothing explaining the lack of the table in the annex or handbook commentary 
that I can see.

The table was titled Palletized, solid-piled, bin box, shelf, or back to back 
shelf storage of class 1 through class 4 and cartoned unexpanded commodities.


My educated guess is that someone figured out that solid shelves don't do so 
well in these situations.

I checked in 2019 as well, not in there either.

RIP back-to-back shelf storage 6 EC head calcs with 250 GPM hose I guess.

Benjamin Young
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: partial systems - running piping through unprotected areas

2019-07-16 Thread Larry Keeping
I think the section that you might be looking for is in A.8.1 of NFPA 13-2013.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: July-15-19 7:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: partial systems - running piping through unprotected areas

My memory is failing me today.  Isn't there a section that says I can't run 
piping through un-protected areas?  We have a building that has a partially 
protected basement.  Basically, we have to bulk across the basement to protect 
3 areas.  Can some one help me find the section of 13 that says this is 
acceptable or not?

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Storage of motorcycle tires

2019-07-13 Thread Larry Keeping
This is just my opinion, but just because the definition doesn't reference 
motorcycle tires (or ATV tires for that matter, or the one on my wheel barrow) 
doesn't negate the fact that motorcycle tires are rubber tires. That definition 
doesn't comply with the NFPA Manual of Style either, so the definition is 
definitely flawed.

However, in Chapter 18 of NFPA 13-2013 (for example) tires on racks on tread 
are covered, so I don't think you really have a problem with design criteria.

Larry Keeping


From: Sprinklerforum  On Behalf 
Of David Bitton
Sent: July-12-19 4:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Storage of motorcycle tires

I am looking at a storage area for motorcycle tires on fixed racks on tread.  
NFPA 13 excludes such tires from its definition of rubber tires (FM 8-3 does 
not). I would like your opinion about how to determine protection criteria for 
this storage?  (Miscellaneous storage does not apply.)
Thanks,

David Bitton, ing./Eng.
Quest Loss Control Services Inc.
Les services de prévention des sinistres Quest
5100, rue de la Savane, bureau 200
Montréal, Québec
H4P 1T8
(514) 341-4545
www.questlosscontrol.com<http://www.questlosscontrol.com/>







___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] Re: Suction Control Valve

2019-06-18 Thread Larry Keeping
Back to the original question of “Who/What determines when a Suction Control 
Valve is needed?”, the AHJ calls for it.

The Handbook for NFPA 20-2013 has the provision from the standard plus some 
explanatory text:

4.15.9   Low Suction Pressure Controls.

4.15.9.1   Low suction throttling valves or variable speed suction limiting 
controls for pump drivers that are listed for fire pump service and that are 
suction pressure sensitive shall be permitted where the authority having 
jurisdiction requires positive pressure to be maintained on the suction piping.

The use of low suction pressure throttling valves is discouraged but permitted 
if required by an AHJ. A low pressure throttling valve reduces the pressure 
available to the fire protection system and provides another potential point of 
failure. When used, a low pressure throttling valve is installed in the 
discharge piping, with the sensing line for the device connected to the suction 
piping. …

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: June-18-19 7:36 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Re: Suction Control Valve

Check out the Bermad FP 436.  It is a “pressure sustaining valve.”  I’ve seen 
water purveyors require these so that you don’t draw the suction line below 20 
psi.  It is installed in the pump discharge.  It also acts as your pump 
discharge check valve.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Mark.Phelps
Sent: Tuesday, June 18, 2019 4:26 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] Re: Suction Control Valve

The 2019 version of NFPA 20 goes on to say : 4.16.5.4   No control valve other 
than a listed OS valve and the devices as permitted in 
4.29.3<https://codesonline.nfpa.org/code/40e1327d-3fd3-4a71-860f-4ec92a4bec89/e909aaad-4058-4ae1-9c1b-0a58441efe7a/np_58253fca-f642-11e7-914a-0547f3f12f9d.html#ID00020544>
 shall be installed in the suction pipe within 50 ft (15.3 m) of the pump 
suction flange. 4.29.3 describes how to install a backflow preventer a minimum 
of 50 feet from the suction flange of the fire pump.
I don’t find anywhere in NFPA 20 where it describes or allows a “Throttle 
Control Valve.
Mark at Aero
602 820-7894



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Timothy Goins
Sent: Tuesday, June 18, 2019 3:28 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: [EXTERNAL] Re: Suction Control Valve

Please re-read my copied text from the
NFPA 20, it says shall be installed on the suction line. Not should, but shall.


And I will give them one heart, and I will put a new spirit within you; and I 
will take the stony heart out of their flesh, and will give them an heart of 
flesh
Eze 11:19

On Jun 18, 2019, at 4:23 PM, Prahl, Craig/GVL 
mailto:craig.pr...@jacobs.com>> wrote:
On marginal municipal water supplies where there is the chance that the fire 
pump could draw flows greater than what could be provided, the water purveyor 
will often request a suction control valve.  Basically, this throttles the flow 
from the pump and keeps the municipal system pressure from going negative.

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg=DfTAYwUJpJ5qWdFrEReH1LUJi7vmhhsyNN16NPQ7H4w=HvVurPrXKAWSL3gbUp-tLO7vWCSKDJaxF9EKKQ1WV5Y=>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Vince Sabolik
Sent: Tuesday, June 18, 

Bags to Protect Sprinklers from Overspray

2019-06-13 Thread Larry Keeping
Can someone please provide a name/location for a supplier of the cellophane 
bags or the thin paper bags, used to protect sprinklers in spray booths from 
overspray.

I remember from years gone by, small bags, just big enough to cover a 
sprinkler, with a thin draw string, to secure the bag in place, but now, at 
least in the Toronto area, no one seems to have a source for them.

Thank you,

Larry Keeping
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Pump Question

2019-06-05 Thread Larry Keeping
Section 6.1.2 of NFPA 20-2019 is pretty clear:

6.1.2*   Application.   Centrifugal pumps shall not be used where a static 
suction lift is required.

When I first started in the FP industry, NFPA 20 allowed horizontal pumps to be 
primed and operate with a suction lift, but, if memory serves, those provisions 
were taken out back in the 1974 or 1976 editions. I understand that there were 
a series of incidents of foot valve failure and lost prime that led to pumps 
running dry and being ruined.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Laleh Zargarinejad
Sent: June-05-19 9:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Pump Question

Is vertical turbine fire pump the only type approved by NFPA for negative 
suction lift? (fire pump above the tank).

I designed one for a high rise in Houston years ago, where we put a diesel 
powered vertical turbine pump over an underground tank (tank was there as 
second source of water supply).

Is there a way to use a centrifugal pump and prime it (in a fashion acceptable 
to NFPA)?

Otherwise I am looking at an underground tank with the vertical turbine pump 
right over it and building a small heated shack for the pump and accessories.

To compound my question, what are the restrictions for a campus-wide type fire 
protection, such as a cluster of 9 small one story buildings (~2,500 sq ft 
each), all R-2 classification(sleeping quarters for the students) + one larger 
bldg. (~10,000 sq ft one story), which has three classrooms , a kitchen and 
dining area (I am not sure if that would be E or A classification, but in any 
event it would be a NFPA-13 vs NFPA 13R for the smaller buildings serving as 
sleeping quarters). All the buildings within a say 150' radius.

The issue here is it may be cost effective to install one fire pump and storage 
tank and serve all 10 buildings, however to provide a separate system for each 
building may become cost prohibitive.

Laleh Zargarinejad
Fire Protection Engineer




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13 (2013ed) figure 15.2.2

2019-05-22 Thread Larry Keeping
As I understand it, the Table is based on test data using ½ and large orifice 
sprinklers, which don’t always give the best results against high piled 
storage, so that could explain some of the inconsistencies.

Having said that though, it looks to me that Column C is generally less 
demanding than Column E.
ie. For 20 ft storage in a 25 ft high building, Col. C wants a 0.60 density 
whereas Col. E wants 0.70.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Dewayne Martinez
Sent: May-20-19 2:50 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez 
Subject: NFPA 13 (2013ed) figure 15.2.2

Group A plastics, 5-12ft of storage, 15 to 20ft ceiling
Figure 15.2.2 / table 15.2.6(a)

Why is Group A, Expanded, Cartoned, Stable (Column E) less of a hazard then 
Group A, nonexpanded, stable, cartoned  (Column C)?
One would think that since the expanded has a higher heat release rate so it 
would be higher density.  Can anyone help me understand this?

Thanks,
Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:image003.png@01D4F47B.AA7F2100]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: definition of "bulk"

2019-05-13 Thread Larry Keeping
Section 22.37 is extracted from NFPA 400.  NFPA 400 has a definition for “Bulk 
Solid Storage” – The storage of more than 6000 lb (2722 kg) in a single 
container.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Travis Mack
Sent: May-13-19 10:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: definition of "bulk"

I believe that when 13 does not define something you are to go to a recognized 
dictionary. So try Webster’s online.

No, the Urban Dictionary doesn’t count.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On May 13, 2019, at 7:53 AM, Zachary Siegrist 
mailto:zachary.siegr...@gmail.com>> wrote:
I am inquiring to see if anyone can provide clarification to the term "bulk" as 
it relates to the storage of solid oxidizers in Table 22.37.1.4.1 (2013 ed.).  
I don't see the term defined in Chapter 3.

Zach Siegrist
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: EC HSW Under Garage Doors

2019-04-05 Thread Larry Keeping
Hi Skyler:

I think you are putting too much thought into the matter. You had it covered 
when you read NFPA 13-2013,  Section 8.9.5.3.2: “Sprinklers shall be installed 
under fixed obstructions over 4 ft (1.2 m) wide, such as ducts, decks, open 
grate flooring, cutting tables, and overhead doors.”

Since Section 8.9 is for Extended Coverage Sidewall Spray Sprinklers, there is 
really no question – they are okay to use there.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Skyler Bilbo
Sent: April-05-19 2:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: EC HSW Under Garage Doors

Thanks!  I need to buy the 2019 version...  I feel like one of those old guys, 
from when I started in the industry, that quotes older versions because those 
are the ones I'm most familiar with... I'm not looking forward to learning the 
new rearranged chapters but I also don't want to be "that guy" who needs to get 
with the times.  Times are definitely changing when a millennial starts having 
old person dilemmas, haha.


Skyler Bilbo


On Fri, Apr 5, 2019 at 1:35 PM Mike B Morey 
mailto:mmo...@shambaugh.com>> wrote:
NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to protect 
areas below a single overhead door(s)

that should cover you



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com<mailto:mmo...@shambaugh.com>

[cid:image001.jpg@01D4EBCC.9325F0E0]





From:Skyler Bilbo 
mailto:sbi...@wenteplumbing.com>>
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Date:04/05/2019 02:31 PM
Subject:EC HSW Under Garage Doors
Sent by:"Sprinklerforum" 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>




BE ADVISED - This email originated outside EMCOR.

Is anyone installing EC HSW heads under garage doors?  I keep running into 16 
ft wide doors (queue jokes: "just open the door").  It would be cheaper to 
install one EC head rather than a standard spray HSW on each side.

I'm looking in the 2013 version of NFPA 13, and I see in 8.4.2 where it allows 
standard sidewall spray sprinklers under garage doors, which isn't mentioned 
for the similar section regarding extended coverage sidewall sprinklers.  It is 
mentioned in the EC HSW section: 8.9.5.3.2 that sprinklers are required under 
obstructions over 4 ft wide such as overhead doors.  I'm thinking this is just 
saying sprinklers are required under the garage door due to the obstruction, 
but not implying that EC HSW can be used.  It seems to me that NFPA is already 
being "nice" to us by letting us use the Light Hazard spacing for these HSW 
heads under garage doors and spacing the heads out farther with EC heads is 
pretty liberal if you are worried about this head ever actually going off in a 
fire.  I would be interested to know if there has been any testing on this.


Thanks,
Skyler Bilbo___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=GKdB6-XpYq_0W-WluyVHtw=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg=JfddSnRHvASLscCAQ7fPAc_hWOQTMOTCFlULHkBP3wY=MCa_hXG8oPD-5QoSupXxx745eXtTyBzVQhCP6FRC0z8=
This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Table Confusion

2019-03-21 Thread Larry Keeping
Oops!Sorry!

I was mistakenly looking at Table 16.2.1.3.3.1 when I references Curves A & B.
In Table 16.2.1.3.3.2 both conditions use Curves C & D, but for encapsulated 
you increase the density by 1.5.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Matthew J Willis
Sent: March-21-19 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Table Confusion

How do we arrive at A and B in the Table?

R/
Matt

Matthew J. Willis, CWBSP
Design Manager /3-D Specialist
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:image001.png@01D159E8.1A3A2D00]

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Larry Keeping
Sent: Thursday, March 21, 2019 7:05 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Table Confusion

You also must also look at other lines of Table 16.2.1.3.3.2.
For nonencapsulated you need 1 level of in-rack sprinklers and you pick your 
density and design area based on Curves C or D.
For encapsulated you need 1 level of in-rack sprinklers and you pick your 
density and design area based on Curves A or B and then you increase the 
density by a factor of 1.5.
Best regards,
Larry Keeping


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matthew J Willis
Sent: March-20-19 7:06 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Table Confusion

NFPA 13 - 2016.
Class IV Encapsulated- 18'-0"

Table 16.2.1.3.3.2 tells me to go to Figure 16.2.1.3.2(d).

The Figure description says "Class IV Nonencapsulated".
But the table has "Yes" for encapsulated.

Is this a typo, or is it just too late in the  day?

R/
Matt

Matthew J. Willis, CWBSP
Design Manager /3-D Specialist
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:image001.png@01D159E8.1A3A2D00]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Table Confusion

2019-03-21 Thread Larry Keeping
You also must also look at other lines of Table 16.2.1.3.3.2.
For nonencapsulated you need 1 level of in-rack sprinklers and you pick your 
density and design area based on Curves C or D.
For encapsulated you need 1 level of in-rack sprinklers and you pick your 
density and design area based on Curves A or B and then you increase the 
density by a factor of 1.5.
Best regards,
Larry Keeping


From: Sprinklerforum  On Behalf 
Of Matthew J Willis
Sent: March-20-19 7:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Table Confusion

NFPA 13 - 2016.
Class IV Encapsulated- 18'-0"

Table 16.2.1.3.3.2 tells me to go to Figure 16.2.1.3.2(d).

The Figure description says "Class IV Nonencapsulated".
But the table has "Yes" for encapsulated.

Is this a typo, or is it just too late in the  day?

R/
Matt

Matthew J. Willis, CWBSP
Design Manager /3-D Specialist
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:image001.png@01D159E8.1A3A2D00]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Water hammer in Dry or deluge systems

2019-03-12 Thread Larry Keeping
I wouldn’t agree that it isn’t a real-world issue. Years ago, I had a deluge 
system in an air craft hanger bend the hangers/supports on the risers during 
the trip testing. Bracing against the impact forces is strongly recommended.

I’ve even seen wet pipe systems mains that shifted out of position, due to the 
client wheeling open control valves and filling them to quickly.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Skyler Bilbo
Sent: March-12-19 10:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Water hammer in Dry or deluge systems

Craig,

I have run into a very similar scenario.  I had a real concern with so much 
water hitting every change in direction and dead end with a lot of force.  All 
of the deluge valves that I know of go from being closed to open full bore, as 
quickly as the clapper can open (fast).  Also, it is important to realize that 
the water will not move through at the designed minimum flow rate, but probably 
much faster.  In our case, we installed seismic bracing at every elbow and near 
any dead ends.  This wasn't engineered, as I'm not aware of any guidelines or 
requirements for designing this bracing.  It seems to me that this is a similar 
concept to thrust block design for underground piping (where the forces in a 6" 
elbow can easily exceed 5,000 lbs and substantially higher than this in larger 
sizes), but there are definitely some differences.  If nothing else, the braces 
provided me with some peace of mind.  I felt it was important to make sure that 
the braces were installed and oriented correctly. I also made sure that no one 
entered the area when we did the startup testing, and everything went well.  
The bracing definitely helped.

Thinking about this more - hopefully someone will chime in... The total 
pressure (velocity pressure + normal pressure) should never exceed your initial 
static pressure.  If you design braces to handle this full initial static 
pressure times the area of whatever size pipe you have (pi * r^2), I would 
think this would be a safe calculation.  Again, I hope someone chimes in on 
this.  I have been wrong more than once, so don't just take my word for it.

I just read Roland's response.  It's good to know it hasn't been a real world 
issue.  I know that I was pretty nervous about it when my name was attached to 
it.  The cost of the braces was worth it to me.


- Skyler

On Tue, Mar 12, 2019 at 8:59 AM Prahl, Craig/GVL 
mailto:craig.pr...@jacobs.com>> wrote:
So, I’ve got an FPE and ME questioning about water hammer in a deluge system.

We have a unique installation where we have two levels of hose connections (one 
array at 12 ft AFF and one at 60 ft AFF) for manual firefighting in an 
unconditioned assembly building which is 145 ft high.

Due to the non-heated condition, one proposed concept for a semi-automatic 
system is to use an electric release deluge valve to charge the system from 
manual pull stations.

Flow rate will be 1,000 gpm at somewhere near 150ish psi though 600-800 ft of 
pipe inside the bldg.

The FPE and ME are concerned with water hammer in the piping when the deluge 
valve opens based on how fast the valve opens.

Has anyone dealt with or had to provide calcs for this?  NFPA 13, 14, etc. are 
fairly silent on the issue.  Is it even an issue?  I’ve never had this brought 
up before on an interior system.

Anyone have any data on how fast a solenoid operated deluge valve opens?

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>




NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Floor Control Drain Pipe SIze

2019-02-21 Thread Larry Keeping
That requirement was first added into the standard for the 1991 edition. The 
substantiation was:
“… By requiring the size to be one pipe size larger than the largest size drain 
connection tying into it, two floors could be drained simultaneously if 
necessary, without causing an excessive delay in draining time.”

Best regards,
Larry Keeping

From: Sprinklerforum  On Behalf 
Of Joe Burtell
Sent: February-21-19 4:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Floor Control Drain Pipe SIze

Can some tell me why NFPA decided to upsize the drain pipe size for floor 
control situations?

16.10.4.8 Where drain connections for floor control valves are tied into a 
common drain riser, the drain riser shall be one pipe size larger downstream of 
each size drain connection tying into it.

To further this discussion, if I have a riser room with 10 riser and the drains 
are all tied together, there is no requirement to upsize that drain pipe that I 
can see. So why one and not the other?

Best regards,

Joe Burtell, SET, CFPS

[Burtell Fire_Small]

Phone | Fax | Mobile| Text 406-204-4653

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com<mailto:j...@burtellfire.com>

Web Site: http://www.burtellfire.com<http://www.burtellfire.com/>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Radiant Heater spacing

2019-01-11 Thread Larry Keeping
As per Table 9.2.4.5(a), Part 2 Unit Heater and radiant heater, Item b, 
Vertical downward discharge, high temperature sprinklers are called for any 
sprinklers within a 7 ft radius cylinder extending 7 ft above and 2 ft below 
the heater. Intermediate rated sprinklers are needed above the 7 ft distance.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Dane Long
Sent: January-11-19 10:27 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Radiant Heater spacing

I noticed theirs not a lot of guidance in NFPA 13 (19 Edition) regarding 
radiant heaters. The only information given is table 9.4.2.5(a) and it states 
that anything within 7ft has to be a 286 degree sprinkler. Is this still the 
case even when the heater is less then 7ft from the roof deck and the deflector 
on the heater is directing the heat down?

Thanks,

Dane Long

Design Tech | Bamford Fire Sprinkler

P: 785-825-7710
F: 785-825-0667

A: 1383 W. North St. Salina, Ks 67401







From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Kyle.Montgomery
Sent: Thursday, January 10, 2019 4:00 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] RE: PRV By-pass

Wait, are you planning to use the ZW4004 as the control valve, with the hose 
valve downstream and no system control valve or check valve? I’m not sure if 
you could do that, because then it’s like the hose valve is coming off the 
sprinkler system. I don’t see it as a problem from a practical standpoint, but 
you could get hung up in a technicality.

When we did it, we had a little manifold with the capped-bonnet ZW4004 then a 
tee to a standard hose valve (non-PRV) then a butterfly valve and check valve 
for the system. Maybe you don’t need the extra check valve and/or butterfly 
valve. What say the peanut gallery?


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Kyle.Montgomery
Sent: Thursday, January 10, 2019 2:55 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] RE: PRV By-pass

This is a legit way to do it. You can get that valve with a capped bonnet if 
you don’t want to have an extra unnecessary control valve.

Travis is thinking of a pilot-operated pressure reducing valve (pressure 
regulating valve?) which is also legitimate, and gives you more residual 
pressure to work with, but costs like 4 or 5 times as much.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Thursday, January 10, 2019 9:56 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
mailto:dmarti...@total-mechanical.com>>
Subject: [EXTERNAL] RE: PRV By-pass

I have never done this before but we were just tossing ideas around to save 
some cash on projects.  We use the 2 ½” Wilkins ZW4004 globe model which is 
good up to 500 gpm.  I would calculate the valve for 250gpm flow and use these 
numbers for both the system and fire hose valve.   What is the PReIV/PRedV?

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmechanical.com_=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=NLaBHhNMlhuwjmHtIwrNKnRXUE6bCAJQ0QJ6fXzzR7U=GIutsxVg2AyCSFwc37VXHwk3wPK2czDtVqaGadAaRWI=>

[A close up of a sign  Description generated with high confidence]

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Thursday, January 10, 2019 10:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: PRV By-pass

Do you have the room for that?  It sounds acceptable, but will be a large 
assembly, presumably in a stair.  Are you selecting a PRedV that works at lower 
flows of a single sprinkler and at the higher flows of the standpipe or 
sprinkler design area?  I believe the Tyco PRV-1 allows for flows from 0 – xxx. 
 That would work for you.  Also, make sure you get the properly sized PRelV 
installed downstream of the PRedV.  Check the PRedV data sheet for size of 
PRelV.

[MFP_logo_F]
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5

RE: Indoor Trampoline Park

2019-01-04 Thread Larry Keeping
I’m not sure how this thread started discussing ESFR sprinklers. As I 
understand it, the sprinklers are 286°F temperature rated and as far as I know, 
ESFRs do not come so rated.

Last May sometime, I believe the NFPA Xchange had a Q & A about “The Emerging 
Hazard of Indoor Athletic Facilities and Trampoline Parks” with Matt Klaus. I 
didn’t take part that session, but it looks from the title that the hazard 
classification for such facilities is now being seriously considered. With 
this, I suggest that a query to the NFPA might be in order, to see what the 
current thinking on the subject now is.

Best regards,

Larry Keeping



From: Sprinklerforum  On Behalf 
Of Parsley Consulting
Sent: January-04-19 11:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Indoor Trampoline Park

Joe,

I believe it's worth mentioning that in the scenario you've described, that of 
a design of an ESFR system in a warehouse when the space is not used for high 
piled storage or is converted to light or ordinary hazard occupancy, that 
23.1.1 of the '19 edition (12.6.7.1 in the '16) notes that if the ESFR system 
were designed to meet the criteria in the ESFR chapter that it "shall be 
permitted" to protectLH, OH, storage protected by OH1, OH2, EH1, or EH2.

There standard give clear guidance that replacing the ESFR system in such a 
circumstance isn't necessary.  It basically agrees with your concept.

sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 01/03/2019 2:01 PM, Joe Burtell wrote:
There is nothing that says you cannot overdesign a system. Case in point is 
ESFR sprinkler systems. We install them in lease warehouses all the time even 
though the current tenant may only be storing class 1 product to 12'-0. Is it 
overkill, yes, but it gives them flexibility for future tenants. Same is true 
in your case. What about the next tenant, maybe OH 2 is more appropriate for 
the next guy. So we should replace systems like we change underwear, well maybe 
for some of us. I may question the temperature of the sprinklers but beyond 
that, just calc it with a boatload of safety if that's what he wants.

Best regards,

Joe Burtell, SET, CFPS

 *PLEASE NOTE NEW PHONE NUMBER*

[Burtell Fire_Small]

Phone | Fax | Mobile| Text 406-204-4653

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com<mailto:j...@burtellfire.com>

Web Site: http://www.burtellfire.com<http://www.burtellfire.com/>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.


On Thu, Jan 3, 2019 at 2:52 PM John Irwin 
mailto:jir...@quickresponsefl.com>> wrote:
Exposed roof at about 25ft. 286 sprinklers are existing.
We have no information on the padding used for the park.
John Irwin
West Coast Branch Manager
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical 
transgressions and grammatical gaffs.


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Prahl, Craig/GVL 
mailto:craig.pr...@jacobs.com>>
Sent: Thursday, January 3, 2019 4:48:09 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Indoor Trampoline Park

Is there a ceiling or exposed construction overhead?  What is the ceiling/roof 
height?  Do any of the foam, vinyl, foam rubber, plastics, etc. have any 
special ratings making them non-combustible or self-extinguishing?  Smoke and 
Flame spread ratings matter with respect to occupant evacuation.

Is there space below the trampolines?  What is being done there to prevent 
debris accumulation?  How would a fire be addressed below the trampoline?

No, you as the sprinkler contractor have nothing to do with the fire alarm 
system and how it functions.  Remember, as the AHJ, they typically cover a 
mul

RE: Hydrostatic Testing

2018-12-12 Thread Larry Keeping
My guess is that you are looking for it in Chapter 28. However, you’ll find it 
in Section 29.7. Chapter 29 covers Existing System Modifications.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Joe Burtell
Sent: December-12-18 11:04 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Hydrostatic Testing

Can anyone tell me why this section is missing from the 2019 of NFPA 13?

25.2.1.4 Modifications to existing piping systems shall require testing at 
system working
pressure.
25.2.1.4.1 Where modification is made to an existing system affecting more than 
20 sprinklers,
the new portion shall be isolated and tested at not less than 200 psi (13.8 
bar) for 2 hours.
25.2.1.4.2 Modifications that cannot be isolated, such as relocated drops, 
shall require testing
at system working pressure.

Best regards,

Joe Burtell, SET, CFPS

 *PLEASE NOTE NEW PHONE NUMBER*

[Burtell Fire_Small]

Phone | Fax | Mobile| Text 406-204-4653

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com<mailto:j...@burtellfire.com>

Web Site: http://www.burtellfire.com<http://www.burtellfire.com/>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Mixed rack storage

2018-11-29 Thread Larry Keeping
Whoa there!

The Chapter 13 only covers plastic to storage to 5 ft in dedicated storage 
facilities or Miscellaneous Storage of Plastics to 12 ft.

My understanding is that the area in question is designated for storage (ie. it 
is a 4600 sq ft warehouse area), so for plastics to 12 ft on racks you need to 
go to Chapter 17.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of John Irwin
Sent: November-29-18 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Mixed rack storage

I agree with this, except it calls for one level of in-racks.

John Irwin
Quick Response Fire Protection

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of cw bamford
Sent: Thursday, November 29, 2018 10:36 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Mixed rack storage

Calc seperate areas.

group A plastics on racks UNDER 12’

using 2013 edition of NFPA 2013
Table 13.2.1
Exposed -- Unexpanded --  Rack
>10' to 12'
OH2

Please check my work.

onto
Ceramic Floor Tiles
It's not just the commodity, It's how they are stored and moved on the racks
? in cardboard ? with some Styrofoam? Encapsulated? solid shelves

Chuck Bamford SET



On Wed, Nov 28, 2018 at 11:05 AM John Irwin 
mailto:jir...@quickresponsefl.com>> wrote:
I am working on a flooring retail building that has a 4,600 sqft warehouse. 
Roof is at 30’ and they want to store to 20’. They will have vinyl flowing and 
rolls of rug and carpet, as well as ceramic and porcelain tile. I believe I 
have determined that the vinyl and rolls of rug equate to Group A, non-expanded 
plastics. My question is this … is it permissible for the client to storage all 
their group A plastics on racks UNDER 12’ and their ceramic floor tiles on the 
racks OVER 12’ and to then calculate the roof system for the lesser, ceramic 
tile storage?



John Irwin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pallet storage above overhead doors

2018-11-14 Thread Larry Keeping
I'm out of touch with the FM data sheets these days, but from an NFPA 13-2013 
perspective, I think Sections 12.1.3.3 and 12.12.3.3 would come into play:

12.1.3.3   The sprinkler system design shall be based on the storage height and 
clearance to ceiling that routinely or periodically exist in the building and 
create the greatest water demand. Where storage is placed above doors, the 
storage height shall be calculated from the base of storage above the door.

12.12.3.3   Where idle pallet storage is above a door, the idle pallet storage 
height and ceiling height shall be calculated from the base of storage above 
the door using the applicable protection criteria referenced in Section 12.12.

>From this, I would conclude that the sprinkler protection for 6 ft of idle 
>wood pallets from Tables Table 12.12.1.2 (a) (b) or (c) would be called for. 
>For idle plastic pallets, compliance with Section 12.12 would be needed.

It should be recognized that the above is just my personal opinion, and has not 
been processed as a formal interpretation in accordance with the NFPA 
Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA, nor any of 
their technical committees.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of James Crawford
Sent: November-13-18 3:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Pallet storage above overhead doors

We are working on a project where the tenant wants to store pallets above the 
overhead loading doors to a height of 6'-0" in the loading dock area..

The project will be using Factory Mutual data sheets, so I went to DS8-24 Idle 
Pallet Storage and because they are on racks it send me to DS8-9 and 8-9 tells 
me to use rack storage for Un-cartoned, un-expanded Group "A" plastics Table 10.

Based on the height of the building (40'-0") I would need ESFR K25 operating at 
60psi to protect 6'-0" of wooden pallets, this seems a little excessive.

So if we add a level of in-racks sprinkler heads and use Table 13 we would have 
5' to 10' storage above the sprinkler and 10' to 20' clearance above the top of 
the pallets. So this tells me to use the 15' storage from Table 10 or ESFR K25 
@ 25psi plus 1 level of in-racks. Still seems a little excessive.

Am I reading this right?


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: corridors and residential sprinklers

2018-10-29 Thread Larry Keeping
Take a look at NFPA 13, Figure A.11.3.1.1(a), Examples of Design Area for 
Dwelling Units.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of NSFD
Sent: October-29-18 8:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: corridors and residential sprinklers

I would go w/ the four sprinklers. Section 8.4.5.1 permits residential 
sprinklers for dwelling units "and their adjoining corridors" and I think 
that's the key to get you into 11.3.1 for calculations. (2013 edition 
references).

On Mon, Oct 29, 2018 at 5:09 PM MFP Design, LLC 
mailto:tm...@mfpdesign.com>> wrote:
For a project that is a “typical” apartment building protected by NFPA 13 using 
residential sprinklers, how many sprinklers do you calculate in a corridor.  In 
the NFPA 13 handbook, it says that when doing room design method, you can 
consider the corridor a room and calculate 5.  However, the handbook goes on to 
state that you can’t use room design for residential sprinklers and you must 
calculate 4 sprinklers.  This may require going to adjacent rooms if necessary.

So, since we can’t use room design for the corridor and residential sprinklers, 
it would seem that you would only calculate 4.  To eliminate the 75’ max 
argument, let’s say the sprinklers are spaced at 16’ on center.  So, do we 
calculate 4 or 5 residential sprinklers in a corridor?  This came up in a 
discussion today.

Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ball drip valve

2018-10-05 Thread Larry Keeping
I am afraid I don’t entirely understand your last message. If water is leaking 
past the ball drip, it means there is a problem at the air or water seats. As 
per my previous message, that needs to be corrected. Getting the ball valve to 
seat to stop the leakage is not a solution to the problem.

Larry

From: Sprinklerforum  On Behalf 
Of Douglas Hicks
Sent: October-05-18 12:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ball drip valve

Thanks Larry.  I have installed  ball drip valves, with and without the push 
rod.  I have used a pen to push the ball back on those ball valves without the 
push rod.  I found that usually stops the
the leaks

From: Larry Keeping<mailto:lkeep...@plcfire.com>
Sent: Tuesday, October 02, 2018 5:07 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Ball drip valve

If I understand you correctly, the ball drip that is installed is the automatic 
type, which is not right for the trim on a dry pipe valve. The valve should be 
of the mechanical type with a plunger that can be pushed to unseat the valve.

Normally the valve should be unseated with no pressure behind it to cause it to 
seat. The valve is part of the the alarm line drain configuration. After an 
activation/valve trip, the water pressure in the alarm line would force the 
ball onto the seat. To drain it, as part of resetting the DPV, the plunger is 
pushed and held until the alarm line is fully drained.

After resetting the DPV, the plunger is pushed again, to make sure there is no 
water in the line. If there is, that means that there is a leak at the clapper 
gasket/air seat, which must be rectified.

I hope this helps with your problem.

Larry Keeping




From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Douglas Hicks
Sent: October-01-18 12:45 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Ball drip valve

I have a dry system that we change the 1/2”ball drip valve about every 6 
months.  There is no spring in the valve, it is straight through.  Normally, if 
I have a problem with the valve resetting, I put my finger at the outlet and 
the ball is moved against the seat, and the ball seats.

Any hints on how to get the ball to seat?

Douglas Hicks
General Fire Eq of Eastern Oregon, Inc

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ball drip valve

2018-10-02 Thread Larry Keeping
If I understand you correctly, the ball drip that is installed is the automatic 
type, which is not right for the trim on a dry pipe valve. The valve should be 
of the mechanical type with a plunger that can be pushed to unseat the valve.

Normally the valve should be unseated with no pressure behind it to cause it to 
seat. The valve is part of the the alarm line drain configuration. After an 
activation/valve trip, the water pressure in the alarm line would force the 
ball onto the seat. To drain it, as part of resetting the DPV, the plunger is 
pushed and held until the alarm line is fully drained.

After resetting the DPV, the plunger is pushed again, to make sure there is no 
water in the line. If there is, that means that there is a leak at the clapper 
gasket/air seat, which must be rectified.

I hope this helps with your problem.

Larry Keeping




From: Sprinklerforum  On Behalf 
Of Douglas Hicks
Sent: October-01-18 12:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Ball drip valve

I have a dry system that we change the 1/2”ball drip valve about every 6 
months.  There is no spring in the valve, it is straight through.  Normally, if 
I have a problem with the valve resetting, I put my finger at the outlet and 
the ball is moved against the seat, and the ball seats.

Any hints on how to get the ball to seat?

Douglas Hicks
General Fire Eq of Eastern Oregon, Inc
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 13R Test and Drain Question

2018-09-20 Thread Larry Keeping
We can always agree to disagree. From my perspective:


  *   6.10.2 says: The test connection pipe shall be at least 1 in. (25 mm) 
nominal diameter and terminate in an orifice equal to or smaller than the same 
size as the smallest sprinkler installed in the system.
  *   6.10.3 says: A valve shall be installed in the test connection piping.

And then:


  *   6.10.4 says: When the drain required in 6.9.1 is arranged as a test 
connection (ie. as per the above), a separate test connection isn’t required.

When I read what is in the standard, I don’t see anything about a test port 
being taken off the drain line.

So, as I see, it if you configure your drain in accordance with 6.10.2 & 
6.10.3, the assembly can serve as both the drain and the test pipe.

Just my personal opinion.

Best regards,

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Ron Greenman
Sent: September-20-18 11:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 13R Test and Drain Question

Larry, I’d disagree with that interpretation as the minimum drain size is 1 
inch. I believe that “connection” is the key word here asboth drains and test 
piers are not part of the system but attached to it. I think what’s being said 
is you can take the test port off of the drain line if properly configured 
rather than need a separate connection to the system.

On Thu, Sep 20, 2018 at 8:41 AM Larry Keeping 
mailto:lkeep...@plcfire.com>> wrote:
I would say that test pipe would do the job, based on what it says in 6.10.4:

6.10.4 When the drain required in 6.9.1 is arranged as a test connection, a 
separate test connection shall not be required.

Larry Keeping

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of James Litvak
Sent: September-20-18 11:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: 13R Test and Drain Question

On a 13R system, 6.9.2 specifies that the drain piping must be at least 1" 
nominal size. If a residential system riser has a 1" drain pipe to outside that 
has either a test valve with a 1/2" orifice or terminates at a broken sprinkler 
with a 1/2" orifice, does that drain piping still meet the requirements of 
6.9.2?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 13R Test and Drain Question

2018-09-20 Thread Larry Keeping
I would say that test pipe would do the job, based on what it says in 6.10.4:

6.10.4 When the drain required in 6.9.1 is arranged as a test connection, a 
separate test connection shall not be required.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of James Litvak
Sent: September-20-18 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: 13R Test and Drain Question

On a 13R system, 6.9.2 specifies that the drain piping must be at least 1" 
nominal size. If a residential system riser has a 1" drain pipe to outside that 
has either a test valve with a 1/2" orifice or terminates at a broken sprinkler 
with a 1/2" orifice, does that drain piping still meet the requirements of 
6.9.2?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinkler heads popping off randomly

2018-09-14 Thread Larry Keeping
Good morning:

I was late getting to the office this morning, so I am joining in a little 
late. If I remember correctly though, Reliable did have a problem with some of 
their sprinklers back in the mid 60’s, where the links had a fault, such that 
they would pull apart.

After being in place for 50 years +/- it likely isn’t that though. The company 
I used to work for started having problems with them in the late 60’s & early 
70’s, but I think the suggestion to contact Reliable is good advice.

Something that could be done is a visual examination of as many of the 
sprinklers there as is practical, to look for possible defects.

Again, after being there for 50 years +/- the most effective solution may just 
be to replace sprinklers.

Larry Keeping

From: Sprinklerforum  On Behalf 
Of å... 
Sent: September-14-18 3:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly



Larry:

You are getting the best guesses from some of the best and most experienced 
minds in the business.
On a question with a large uncertainty such as this one,  this forum 
(crowdsourcing) is the state-of-the-art strategy for vetting answers.
No single answer seems to be obvious...though Fpdc nicely packaged the options 
into 4 categories.
Since state of the art guessing is better with discussion and full 
participation, I throw my guess into the hat.

  *   random mechanical damage inflicted by installers at various points as 
they completed the job
  *   if all unwanted activations happened at night, it might be that slight 
contraction of the metal upon cooling (versus elongation during a relatively 
hotter day) allows just enough wiggle
  room to promote a release.  This theory would not be supported if any 
of the releases occurred during winter months, however.

I would be SLOWW  to replace an entire warehouse's inventory of 
sprinklers.  Statistically, what Larry is experiencing is VEYYY rare.   We 
in the business have
   heard FM Global claim something like 1 in x million chance of just this type 
of event occuring.  Sprinklers stastically take a kicking and keep on ticking, 
for 60, 80, a 100 years.  There have
   been exceptions however, and that is what drives the interest in this thread.

Scot Deal
Excelsior Risk & Fire
gms:  +420 606 872 129  (GMT + 2)


On Fri, Sep 14, 2018 at 7:54 AM Fpdcdesign 
mailto:fpdcdes...@gmail.com>> wrote:
If sprinklers are activating without a fire situation, there are pretty much 4 
options, over pressurization, overheating, mechanical defect or mechanical 
damage. You have to start with one and go through each to find out what is 
going on (problem solving 101). Start with the PRV. That could eliminate one 
issue and is required on all new grid systems anyway. If you suspect 
overheating, you can do recording thermometers at the ceiling. Mode mechanical 
damage,
You have to look at what is in the are that can cause an issue. (I had a client 
who was having accidental discharges at one particular sprinkler in a freezer. 
When we put an air deflector from the  coping unit, it stopped the problem. 
I’ve crystals from the defrost cycle). If all else fails

I am assuming that you have multiple systems within each building and problems 
with each of them.



On Sep 13, 2018 at 9:02 PM, mailto:sco...@ffcdi.com>> wrote:
Band-Aid and conceivably a waste of money.

Sprinklers are tested at very high pressures, surges aren’t going to randomly 
operate sprinklers.

Should the system have a pressure relief valve, probably yes. Is that the 
solution here, most likely, no.

Scott

Office: (763) 425-1001 x2
Cell: (612) 759-5556

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Fpdcdesign
Sent: Thursday, September 13, 2018 7:57 PM
To: Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: Re: Sprinkler heads popping off randomly

Contact the sprinkler contractor that services you systems. That should be able 
to steer you in the right direction. They can be added at the riser and will 
prevent over pressurization



On Sep 13, 2018 at 8:48 PM, mailto:larry.stew...@earthlink.net>> wrote:
Is the relief valve like a overgrown plumbing PRV? Stupid by nature but 
effective at preventing a calamity? … and starts dripping for no reason? ☺


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Thursday, September 13, 2018 5:31 PM
To: Sprinklerforum
Subject: Re: Sprinkler heads popping off randomly

A relief vale would be a good place to start. That could tell you if it is a 
pressure or temperature problem.


On Sep 13, 2018 at 6:29 PM, mailto:larry.stew...@earthlink.net>> wrote:
Blown heads have been located at branch ends, some near a riser, most in the 
middle somewhere.  Not sure about “lower water usage has dimensioned 

RE: No Jockey Pump

2018-08-29 Thread Larry Keeping
NFPA 20 has never mandated jockey pumps.

Back in the cycle for the development of the 1999 edition, in response to 
Proposal 20-36, the Committee Statement confirmed that "A pressure maintenance 
pump is not required by the standard. ..."

For the 2016 edition, some text was added, for the first time, to clarify that 
pressure maintenance is required for pressure-actuated fire pumps, but a jockey 
pump is not necessarily required to accomplish the task. Section 4.26.1 (c) 
allows "Another approved means that is not the main fire pump". And again, the 
Committee Statement confirmed "... a pressure maintenance pump may not 
necessarily be required and that other forms of pressure maintenance may be 
used. ...".

Larry Keeping



From: Sprinklerforum  On Behalf 
Of Thomas Reinhardt
Sent: August-29-18 5:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: No Jockey Pump

Hi group,
Found a 50 yr. old fire pump at a business that didn't have a jockey pump. Am I 
missing something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
thomas.reinha...@skokie.org<mailto:thomas.reinha...@skokie.org>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: maximum sprinkler system sizes

2018-08-15 Thread Larry Keeping
You might be interested to know that the NFPA 13 Installation TC considered a 
proposal 13-122 for larger system sizes in the ROP meeting for the development 
of NFPA 13-2010. The TC rejected that proposal and issued a committee statement:

“System size limits have a long and successful history that the committee is 
reluctant to change. The potential for much larger systems to be out of service 
during testing, inspections and maintenance events speaks against increasing 
system sizes.”

Larry Keeping

From: Sprinklerforum  On Behalf 
Of Matt Grise
Sent: August-14-18 5:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: maximum sprinkler system sizes

I was recently discussing the max system size issue with a building official. 
In this specific application we are requesting that the AHJ allow us to use a 
60,000 square foot maximum size for ESFR systems in a big box warehouse.

I have commentary directly from FM (in addition to FM2-0) that says “The size 
of the sprinkler system is not expected to affect the effectiveness of the 
sprinkler system as long as the system is designed properly for the occupancy.”

The AHJ’s response was: “The system will work as well when the system is in 
operation, but when you turn it off for maintenance, there is a greater risk of 
fire since there is more area out of service.”

I had assumed that the greater system sizes result in equal system 
effectiveness on the whole – in the sense that there is no evidence that the 
greater system area causes more fire losses even when maintenance downtime is 
factored into the equation. I had even thought that perhaps system performance 
on the whole would be improved since there are fewer control valves in the 
building that could be left closed (when they should be open).

But, I have heard that “assuming” things can have negative consequences…

On that note, I wanted to reach out and see what insight anyone might offer on 
system performance related to system size. Do large sprinkler systems perform 
equally only when they are operating properly – or do they operate properly 
(and perform equally) just as well, historically, as smaller systems? Has 
larger system size ever been faulted as the cause of a loss?

Any insight/research/documentation would be great!

Thanks,

Matt

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved Flange Adapters

2018-07-10 Thread Larry Keeping
I agree, the dimensions don’t work, but also, while it doesn’t say why, the 
Vic-Flange Adapter Notes in Vic. data sheet 10.04 says “FireLock Flange adapter 
should not be used on FireLock fittings.”

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Kenneth Berman
Sent: July-10-18 11:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Grooved Flange Adapters

there's not enough clearance for two on the same 90, and the adapter / coupling 
combo must use a 009 (slip in) coupling.

On Tue, Jul 10, 2018 at 10:29 AM, Brad Casterline 
mailto:bcasterl...@fsc-inc.com>> wrote:
Do 6” Grooved Flange Adapters work on both ends of 6” Firelok 90s?

Thanks,

Brad

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ceiling Grids and Flex Drops

2018-06-04 Thread Larry Keeping
Just a bit of history, if I may.

The current requirements covered by 9.2.3.4.4.1, 9.2.3.4.4.4 and 9.2.3.5.2.2 
originally went into the 1987 edition of NFPA 13 based on testing and a 
proposal from NFSA. Here is the substantiation for TCR 13-97:

SUBSTANTIATION: Tests conducted by the National Fire Sprinkler Association 
(NFSA) show that, in certain instances, pendent sprinklers operating at higher 
pressures create a thrust which can lift the branch line piping. At the end 
sprinkler, the amount of thrust is sufficient to lift a pendent sprinkler out 
of the ceiling tile and up into the concealed space. (See test data).
The unsupported lengths proposed to be permitted within 3-15.5.5.2 and 
3-15.5.5.3 are intended to limit upward movement of the sprinkler within the 
ceiling to approximately 1/8 inch.
The NFSA is continuing to study this subject and may present additional 
recommendations during the public comment period.
NOTE: Supporting material available for review at NFPA Headquarters.

Best regards,

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: May-31-18 7:12 PM
To: sprinklerforum@lists.firesprinkler.org; Mitchell, Scott 

Subject: Re: Ceiling Grids and Flex Drops

Scott,

I agree completely.  Thanks for sharing that video, and it does identify quite 
clearly that when they're installed properly the Flex Heads supplying 
sprinklers will resist the resulting forces and remain in the installed 
position. Pretty decent proof of their response.

This does make me think over the provisions in §9.2.3.4.4.1, §9.2.3.4.4.4, 
§9.2.3.5.2.2, and §9.2.5.4.2 with respect to upward motion or thrust that were 
placed in the standard, probably by some stodgy old TC members who need to be 
voted out.

There is some provision in the standard in §9.2.1.3.3.3 which requires any 
flexible drop fitting longer than 6' is provided with a hanger.  For such a 
stodgy old TC member my memory of that discussion was that it was quite 
"energetic" and was a frank exchange of contrary ideas at high decibel levels.

just my memories,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 05/31/2018 2:45 PM, Mitchell, Scott wrote:

https://www.youtube.com/watch?v=n5fJ1lCVE98



Looks like a decent kick to me.



Scott



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Misc Rack Storage

2018-05-17 Thread Larry Keeping
Just a word of caution.

When you are using 23.4.4.1.1.4, you also have to have additional flow added 
in, as per the corresponding 23.4.4.1.1.5 (see A.23.4.4.1.1.4).

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: May-17-18 11:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Misc Rack Storage

Thanks everyone.

John Irwin
DynaFire Inc. – “Same Day – Next Day”

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton
Sent: Thursday, May 17, 2018 11:36 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Misc Rack Storage

What Craig and Travis said.  From a performance perspective, I always liked the 
“double density” approach where you prove the required density for the hazard 
that mostly characterizes the use and then a smaller hot spot for the more 
hazardous aberration.  So EH2 per Chapter 11, and also a .6/900 sq. ft. or 
something like that.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of MFP Design, LLC
Sent: Thursday, May 17, 2018 8:29 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Misc Rack Storage

When you have mixed criteria areas, you need to extend the higher density into 
the lower density area for 15’.  Reference NFPA 13: 12.3 for that requirement.  
Also, don’t forget the issue of complying with 23.4.4.1.1.4.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Irwin
Sent: Thursday, May 17, 2018 8:23 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Misc Rack Storage

Regardless of the trailers, do I need to provide .6/2000 for the racks? If so, 
do I need to do that for the entire 5,000 sqft area? Seems excessive.



John Irwin
DynaFire Inc. – “Same Day – Next Day”

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton
Sent: Thursday, May 17, 2018 11:19 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Misc Rack Storage

I tend to agree – trailers potentially shielding fire load within from 
sprinklers above (5.4.2).

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Thursday, May 17, 2018 7:06 AM
To: Sprinklerforum
Subject: Re: Misc Rack Storage

Wouldn’t the trailer storage bring it up to EH2?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)

On May 17, 2018 at 9:47 AM, mailto:john.ir...@dynafire.com>> wrote:
Here’s the situation … I have a 5,000 sqft, (currently) ordinary hazard mixed 
use space. The new tenant intends to store two emergency disaster management 
trailers in this space. However, along two walls, they want to put a 3-teir 
rack with storage up to 20’ in height. TOS in the center of the unit is 23-9.

The racks will contain a mix of group A plastic, emergency supplies in plastic 
totes, with lids, on no

RE: Grounding Electrical Wire to Sprinkler System

2018-05-10 Thread Larry Keeping
NFPA 13 - 2016: Section 8.18 & Section 10.5.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Hairfield
Sent: May-10-18 2:28 PM
To: Sprinkler Forum <sprinklerforum@lists.firesprinkler.org>
Subject: Grounding Electrical Wire to Sprinkler System


Where in NFPA 13 does it say that the sprinkler system can not be used to ground

the electrical system?



Thanks,



Mike
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Concrete Pan Construction

2018-04-27 Thread Larry Keeping
The 1” to 6”  with the maximum of 22” requirements have been with us since they 
introduced the obstructed construction concept in the 1991 edition of NFPA 13.

Prior to that, the requirement for beam and girder construction was for 
sprinklers under beams to be 1” to 4” with a maximum of 20”.

Best regards,

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, SET
Sent: April-27-18 12:48 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Concrete Pan Construction

I have existing sprinklers under concrete pan (obstructed) construction that 
are located 22” below the deck.  My concern is that the “beams” are 10” deep.  
That means the deflectors are not within 1-6” of the bottom of the structural 
member.  Am I not applying the correct arrangement from NFPA 13, 2013 ed. 
8.6.4.1.2?  I believe (1) is the only arrangement that works for this scenario. 
 Was the 1-6” below the bottom of the structural member added in recent years?

Thank you.

Reed Roisum


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Church Worship Platform Concealed Space

2018-03-29 Thread Larry Keeping
This is just my opinion, but NFPA 13-02013, Section 8.16.6.2 requires that  
"(a) The space is inaccessible ..." and "(c) The floor ... is tight 
construction" in order to not provide sprinklers

With the introduction of those hatches, both of these conditions are violated, 
so I think that sprinklers in the platform are required, unless one of the 
other concealed space exceptions under 8.15.1.2, (such as having less than 6" 
between the floor and the U/S of the joist) can be met.

Larry Keeping


 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ed Kramer
Sent: March-29-18 10:20 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Church Worship Platform Concealed Space

You might be able to apply section 8.15.6 (2013 edition).If so, be aware
of section 11.2.3.1.4(3).

Ed Kramer
Bamford Fire

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of P & P Sprinklers Ltd
Sent: Thursday, March 29, 2018 8:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Church Worship Platform Concealed Space

We have a church that has a platform 16" High wood construction. They will be 
adding hatches for access just to run AV cabling. Will not be used for storage. 
the platform is roughly 1600 sq ft. Would sprinkler be required even with just 
a few hatched to access the cabling?

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 30% increase for Sloped ceilings

2018-03-27 Thread Larry Keeping
The rule for increasing the design area by 30% for sloped ceilings (greater 
than 2 on 12, was first appeared as Section 5-2.3.2.5 of the 1996 edition.

The Tech Committee added it in via ROP Proposal 13-130.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of cw bamford
Sent: March-27-18 5:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 30% increase for Sloped ceilings

NFPA 13  1994   5.2.3.2.3  has it...

On Tue, Mar 27, 2018 at 1:57 PM, Reed A. Roisum, SET 
<raroi...@kfi-eng.com<mailto:raroi...@kfi-eng.com>> wrote:
It is in 1996.  5-2.3.2.5
Can’t find it in 1989.  I don’t have a 1994 or 1991.


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903<tel:(701)%20552-9903> | mobile: 
701.388.1352<tel:(701)%20388-1352> | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Fpdcdesign
Sent: Tuesday, March 27, 2018 3:46 PM
To: Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: Re: 30% increase for Sloped ceilings

I think 1996. It’s in 1999 and wasn’t marked new but not in the 1994 edition. 
(1996 is missing from my collection)

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:(860)%20535-2080> (ofc)
860-553-3553<tel:(860)%20553-3553> (fax)
860-608-4559<tel:(860)%20608-4559> (cell)


On Mar 27, 2018 at 4:39 PM, mailto:tm...@mfpdesign.com>> wrote:
What year did the 30% increase for sloped ceilings come into NFPA 13?  I’m 
trying to do keyword search but no luck at this time.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271<tel:(480)%20505-9271>
fax: 866-430-6107<tel:(866)%20430-6107>
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Supporting pipe in bottom of pre-cast trench

2018-03-16 Thread Larry Keeping
It is different from when you hang with a rod and ring from the top/ceiling. 
Hangers are tested and listed for conditions of tension, with the weight/load 
being applied downwards. However, you were proposing to use a riser clamp 
rodded upwards from the trench floor, which is outside of the listing 
parameters for the riser clamp and putting the rods under a compression/bending 
load. Perhaps if the rods are short enough or if you stiffen them somehow they 
can support the NFPA 13 design loading requirements, but the applicable part of 
the standard for this is still 9.1.1.2 (Eng. Cert.)

On the subject of Section 9.2.6, I would advise getting an okay from the AHJ 
before proceeding without the Eng. Cert. The 2016 edition isn't referenced in 
your Building Codes yet is it? The 2010 and earlier editions say that pipe 
stands have to be approved, so that means the AHJ's acceptance is needed. Most 
AHJ's will accept a P.E. design, but without that ...

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ben Young
Sent: March-15-18 7:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Supporting pipe in bottom of pre-cast trench

Good point.  Based on John's reference to 9.2.6 in the 2016 edition, and 
specifically 9.2.6.3.2 for short pipe stands, I'm thinking I should be OK 
without a PE certification as long as I meet all the general requirements of 
9.2.6.
So we may just need to go back to a very short traditional pipe stand with the 
U-bolt for restraint.

Larry, for the riser clamp idea, I get what you're saying, but I'm wondering 
how this would be any different (or worse) than supporting the pipe from a 
regular ring hanger and a single piece of ATR, which we would normally do if we 
could support this from the top of the box.
We've done this before with smaller pipe in subfloor spaces for pre-action 
systems, but never for this large a pipe. Our plan was also to use 3/4 or 1" 
pipe sleeves over the ATR to help reinforce them as well.



Benjamin Young

On Wed, Mar 14, 2018 at 3:16 PM, Larry Keeping <lkeep...@plcfire.com> wrote:

> All of the suggestions I've seen in this thread (Fig. 103, Unistrut 
> clamps, etc.) are good offerings, but don't forget, those things are 
> not listed, so to use them legitimately they need an engineer's 
> certification, as per Section 9.1.1.2 of NFPA 13-2013.
>
> Unless you can get an Eng. Cert. for it, I would avoid the riser clamp 
> idea. A deluge system will develop some healthy thrust forces up and 
> down the length of the main, which could bend the vertical support rods.
>
> Larry Keeping
>
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] On Behalf Of Mike B Morey
> Sent: March-14-18 2:49 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Supporting pipe in bottom of pre-cast trench
>
> You might also look at the Anvil 103 depending on space available.
>
>
>
> Mike Morey
> CFPS 3229 • NICET S.E.T. 123677
> Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR 
> Company
> 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 / 
> cell 260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com
>
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/fc5849e0/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Supporting pipe in bottom of pre-cast trench

2018-03-14 Thread Larry Keeping
All of the suggestions I've seen in this thread (Fig. 103, Unistrut clamps, 
etc.) are good offerings, but don't forget, those things are not listed, so to 
use them legitimately they need an engineer's certification, as per Section 
9.1.1.2 of NFPA 13-2013. 

Unless you can get an Eng. Cert. for it, I would avoid the riser clamp idea. A 
deluge system will develop some healthy thrust forces up and down the length of 
the main, which could bend the vertical support rods.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike B Morey
Sent: March-14-18 2:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Supporting pipe in bottom of pre-cast trench

You might also look at the Anvil 103 depending on space available.



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA Technical Question Response [ ref:_00D5077Vx._5005013DQXS:ref ]

2018-03-13 Thread Larry Keeping
I agree with the NFPA response, but one thing I question is, why did the 
contractor assume 20 sq. ft. of coverage area for the sprinklers in that pocket?

By the S x L rule, from NFPA 13-2016, Section 8.5.2, using the dimensions that 
you've reported:

-  S = 11'-5½", which is the distance between the sprinklers along the line ; 
and
-  L = 4'-0", which is two times the 2'-0" distance of the line from the wall 
(which is greater than the distance of 1'-2" from the beam).

So by my math, A = S x L = 11.46 ft x 4.0 ft = 45.84 sq. ft.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Chris Born
Sent: March-13-18 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fwd: NFPA Technical Question Response [ 
ref:_00D5077Vx._5005013DQXS:ref ]

Here is the response I received from NFPA concerning my “area of coverage” 
question last week. Subsequent conversation confirmed other replies on the 
forum to this question that if the sprinkler can’t spray past the obstruction 
you only have to measure to the obstruction.

Sent from my iPad

Christopher H. Born, P.E.
Director, Fire Protection Engineering|Principal Clark Nexsen
4525 Main Street, Suite 1400
Virginia Beach, VA 23462
(757) 455-5800
(757) 961-7933 (direct)
(757) 644-8581(mobile)

Begin forwarded message:

> From: NFPA Systems <techquessyst...@nfpa.org>
> Date: March 13, 2018 at 9:18:17 AM EDT
> To: "fireph...@cox.net" <fireph...@cox.net>
> Subject: NFPA Technical Question Response[ 
> ref:_00D5077Vx._5005013DQXS:ref ]
> 
> 
> 
> I apologize I’m not sure I fully understand your question but if you are 
> asking do you space your sprinkler coverage between beams when sprinklering 
> beam pockets vs trying to use the obstruction rules to spray past the beams 
> then the answer is yes you space to the beams as if they were walls.   
> 
> Important Notice: This correspondence is not a Formal Interpretation issued 
> pursuant to NFPA Regulations. Any opinion expressed is the personal opinion 
> of the author and does not necessarily represent the official position of the 
> NFPA or its Technical Committees. In addition, this correspondence is neither 
> intended, nor should it be relied upon, to provide professional consultation 
> or services.
> 
> Regards,
>  
> Chad Duffy, PE
> Senior Fire Protection Engineer
> NFPA
> 
> If you have a follow-up question directly related to this inquiry, please 
> reply to this email.  If you have another question on either a separate topic 
> or different document please return to the document information pages and 
> submit your new question by clicking on the “Technical Questions” tab.
> 
> --
> -
> Create Date: 3/9/2018
> Contact: Christopher Born
> 
> Subject: Protection area of coverage when spacing is impacted by 
> obstructions
> 
> Question for NFPA: We have a building with exposed structure and some of 
> these beams are deep enough to be obstructions. For both spacing along and 
> between branch lines, the standard states to measure the distance between 
> sprinklers (or to wall or obstruction in the case of the last sprinkler or 
> branch line). The reference to "last sprinkler" in the reference to measuring 
> to an obstruction seems incorrect for both of these sections. Please confirm 
> that the intent is that if there is an obstruction, regardless of location, 
> it is acceptable to use twice the distance to the obstruction for determining 
> the coverage area for a particular sprinkler. 
> 
> We have two review comments from the insurer, one regarding the sprinkler 
> area used in hydraulic calculations and the other concerning the maximum 
> allowable coverage area. In the case of the hydraulic calculation comment, 
> two sprinklers are located within a beam pocket, 11'-5.5" apart, less than 2' 
> from a wall and approximately 1'-2" from a 27" deep beam. The contractor has 
> assumed 20 square feet of coverage area. 
> 
> In the other case, branch lines are located on either side of a 36" deep 
> beam. Sprinklers are spaced a maximum of 12' apart on a line that is 3'-10" 
> from the beam. The other line is 7'-5.5" from the beam and sprinklers are 
> spaced 8' apart. 
> 
> In both of these cases, we believe that the intent of NFPA 13 is to determine 
> area of coverage by measuring to the obstruction and not the next line. 
> Please confirm our interpretation.
> 
> 
> 
> ref:_00D5077Vx._5005013DQXS:ref
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkle

RE: Lumberyard fire flows

2018-02-23 Thread Larry Keeping
My bad. There was a typo in my original message.  I was trying to refer to 
A.31.3.3.2.2,  but I dropped the first "3".

Here is what A.31.3.3.2.2 from the 2018 edition says:

A.31.3.3.2.2   It is recognized that retail and wholesale lumber storage yards 
are normally located within municipal system boundaries, where the system 
should be capable of supplying not less than four 21⁄2 in. (65 mm) hose streams 
simultaneously [1000 gpm (4000 L/min)]. Where large-scale firefighting 
operations can be expected, larger water supplies are needed. Where protection 
from municipal water supplies and hydrant systems is not provided or is not 
considered adequate by the AHJ, a yard fire hydrant system should be provided 
and installed in accordance with NFPA 24.

Larry


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-23-18 10:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

I'm sorry Larry, not following.  Those section numbers not found in the Annex 
of 2015 edition either.

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Friday, February 23, 2018 7:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

I was citing the NFPA 1 - 2015 edition.

Larry

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 5:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

Which edition are you citing?  2018 doesn't have those Annex sections.

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, February 22, 2018 2:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Lumberyard fire flows

2018-02-23 Thread Larry Keeping
I was citing the NFPA 1 - 2015 edition.

Larry

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 5:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

Which edition are you citing?  2018 doesn't have those Annex sections.

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, February 22, 2018 2:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Lumberyard fire flows

2018-02-22 Thread Larry Keeping
NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber. We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread Larry Keeping
Just to clarify, in case anyone wasn't aware, the referenced EC storage 
sprinklers, Tyco TY9128 and the Viking V595, are not ESFR sprinklers.
They are CMDA / CMSA standard response.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Nicky Marshall
Sent: February-12-18 2:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Help Finding ESFR upright greater than K17

Most of the responses do not seem to have answered your question if you are 
specifically looking for an upright ESFR sprinkler.

To my knowledge, the K17 Tyco TY7126 is the biggest upright ESFR unless you go 
Extended Coverage K25: TY9128 and Viking VK595.
If you can go standard response (CMSA) then there are more choices. K17: 
TY7153, TY7151, VK580 and Reliable RA1124.  Then K25 VK598 and Victaulic V4603.


Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2  Mobile: +64 (0)21 433 488  Email: 
ni...@protechdesign.co.nz<mailto:ni...@protechdesign.co.nz>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

"I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody" Lily Tomlin

From: Jeff Polke [mailto:jpo...@gcioutdoor.com]
Sent: Tuesday, 13 February 2018 5:30 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Help Finding ESFR upright greater than K17

Good morning all.  I am looking for an expert in ESFR sprinkler heads to help 
me find a ESFR upright head with at least a K factor 17(not 16.8).  There does 
not seem to be other companies that make these ESFR other Tyco. Please let me 
know.  Thanks.

Jeffrey Polke
Co-President
jpo...@gcioutdoor.com<mailto:jpo...@gcioutdoor.com>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Larry Keeping
The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: January-31-18 4:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Exhaust Air - Paint Booth

2018-01-12 Thread Larry Keeping
I just took a look at what NFPA 33 says about fire protection and ventilation:

9.2  Ventilation Systems.  Air make-up systems and spray area exhaust systems 
shall remain functioning during any fire condition.

9.2.1*  Where air exhausted from spray areas is recirculated, an interlock 
shall shut down the recirculation of air during any fire condition unless it 
can be demonstrated that shutdown creates a greater hazard.

9.2.2   Air make-up systems, spray area recirculation systems, and spray area 
exhaust systems shall be permitted to be shut down and dampers shall be 
permitted to close where the automatic fire protection system type requires 
that ventilation be discontinued.

Does that should answer the question?

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Thom Heller
Sent: January-12-18 1:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Exhaust Air - Paint Booth

As an AHJ, in my jurisdiction, we would want the exhaust air to remain on 
(removal of products of combustion in the event of a fire) while the make up 
air would be discontinued.  Thom

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>;
 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Exhaust Air - Paint Booth

Bruce,

Could you expand on "why" you would want the air to keep running?

Get Outlook for iOS<https://aka.ms/o0ukef>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Bruce Verhei <bver...@comcast.net<mailto:bver...@comcast.net>>
Sent: Friday, January 12, 2018 10:25:17 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Exhaust Air - Paint Booth

Are paint spray operations at this booth supplied by drum or IBC-quantity 
containers located outside the booth? By that I mean as opposed to the more 
common small containers on integral to the hand held spray gun or small inline 
pot.

It's common to use a flow switch to drop power to pump connected to drum on 
waterflow.

Without this fire can attack hose in booth. Pump sees this pressure drop as 
demand for product, and pumps remainder of drum or IBC (intermediate bulk 
container) into booth. Result from a sprinkler design point of view can be 
operation of dozens of heads outside booth. From occupants point of view 
they're now in a fast occurring, if not fast spreading, fire producing dark 
smoke. I assume fully sprinklered building.

I'd ask AHJ what they prefer. Total flood dry chem systems require fan shut 
down. But sprinklers do not. But some AHJ's might require fan shut down. From a 
compliance point of view the AHJ and architect are trying to find a way not to 
count the entire quantity of liquid as being in Use.

As an Alternative Material and Method ruling design, the AHJ has considerable 
sway.

Two questions to resolve early are switch testing and retard setting. 5 seconds 
seems to be adequate to prevent unwanted alarms in my experience.

For the record I would have preferred to leave the fan running. But you should 
call the fire plan reviewer for this project.

Best.

Bruce Verhei

On Jan 12, 2018, at 08:20, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
I would say "probably" but a detection is faster and certainly more 
conventional.  I would actually defer to the electrician or EE who's overseeing 
design/installation of building controls and ask them.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of JD Gamble
Sent: Friday, January 12, 2018 8:16 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Exhaust Air - Paint Booth

Sorry. Yes , spray booth. Flow switch specific to booth.

Get Outlook for iOS<https://aka.ms/o0ukef>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Friday, January 12, 2018 9:14:22 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Exhaust Air - Paint Booth

I assume you mean a spray booth?   Is the flow switch peculiar to sprinklers in 
the booth or will it signal upon flow of any sprinkler in the building in which 
the booth is located?

Steve L.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of JD Gamble
Sent: 

RE: S & L Rule

2017-12-21 Thread Larry Keeping
Who said they wouldn't obstruct heat flow? 
Because they are more than 7.5 ft apart it can be considered to be 
"unobstructed" construction. But of course they are obstructions. 

With unobstructed construction the deflector distance has to be 1" to 12" below 
the ceiling.

You can't space the lines as if the beams don't exist. That is why the spacing 
is across the width of the bays. Since the lines are spaced 1/2 L off either 
side of them, you have sprinklers on either side of them as per 8.6.5.1.2 (2). 
Therefore you don't have to worry about the "Beam Rule (Table 8.6.5.1.2, and 
Figure 8.6.5.1.2(a)).

All I'm saying is that you can space to the beams, bay per bay. You can be 5 ft 
off in the 20 ft bay and 7.5 ft off in the 30 ft bay and under those conditions 
it doesn't matter whether the sprinklers can spray under the beams or not.

Larry

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: December-21-17 8:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: S & L Rule

But Larry, if the beams are not an obstruction to heat flow OR spray pattern, 
it's like they don't exist, no?
Brad.

Quoting Larry Keeping <lkeep...@plcfire.com>:

> You don't need to do anything special with the deflector distance.  
> As per 8.5.2.1.1 (2), the line spacing is to a wall or obstruction:
>
> (2) Between branch lines as follows:
> (a) Determine perpendicular distance to the sprinkler on the adjacent 
> branch line (or to a wall or obstruction in the case of the last 
> branch line) on each side of the branch line on which the subject 
> sprinkler is positioned
> (b) Choose the larger of either twice the distance to the wall or 
> obstruction or the distance to the next sprinkler
> (c) Define dimension as L
>
> The is no argument that the beams that delineate the bays are 
> obstructions. Even if the spray can throw under it, that doesn't 
> change that consideration.
>
> Larry Keeping
>
>
> -Original Message-
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> bcasterl...@fsc-inc.com
> Sent: December-21-17 5:53 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: S & L Rule
>
> I recently learned that the beam only acts like a wall if you can't 
> throw under it, so get those deflectors way up there!
> (Crow and Thunderbird rocks)
>
> Merry Christmas Forum,
>
> Brad.
>
> Quoting Bob <b...@firebyknight.com>:
>
>> The beam is an obstruction that acts like a wall.  You’re covering 
>> floor space, so as long as each sprinkler covers the correct area (30 
>> sf), then the spacing that you are describing sounds in compliance 
>> with NFPA 13 spacing rules.
>>
>>
>>
>> Thank you,
>>
>>
>>
>> Bob Knight, CET III
>>
>> 208-318-3057
>>
>>
>>
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of James Crawford
>> Sent: Thursday, December 21, 2017 3:00 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: S & L Rule
>>
>>
>>
>> We have been having a discussion in the office about the S rule for 
>> spacing of sprinkler heads. We received a sprinkler drawing with some 
>> spacing that we do not agree with, see below, but can find no 
>> specific direction in NFPA #13 (2013) that says it is wrong.
>>
>>
>>
>> Basic situation we have a small building with a 20’ bay and a 30’ bay.
>> Ordinary hazard spacing.
>>
>>
>>
>> For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’
>> off the wall then 10’ between the next line and 5’ to the beam line, 
>> the heads are spaced at 13’ along these lines.
>>
>>
>>
>> Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 
>> off the beam then 15’ between the heads then 7’6 to the wall, heads 
>> are spaced at 8’
>> along the line
>>
>>
>>
>> So our discussion is the sprinkler lines along the beam line which 
>> would be 5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler 
>> heads in the 20’
>> bay are spaced at 13’-0”, so if we use the S rule these heads are 
>> spaced at 12’-6” x 13’-0” or 162.6 ft². Is this correct?
>>
>>
>>
>> And yes I know we could space the 30’ bay with 3 lines at 10’ apart 
>> and that is what I would do but it is not our design.
>>
>>
>>
>> Comments
>>
>>
>>
>> Thank you
>>
>>
>>
>>
>

RE: S & L Rule

2017-12-21 Thread Larry Keeping
You don't need to do anything special with the deflector distance. As per 
8.5.2.1.1 (2), the line spacing is to a wall or obstruction:

(2) Between branch lines as follows:
(a) Determine perpendicular distance to the sprinkler on the adjacent branch 
line (or to a wall or obstruction in the case of the last branch line) on each 
side of the branch line on which the subject sprinkler is positioned
(b) Choose the larger of either twice the distance to the wall or obstruction 
or the distance to the next sprinkler
(c) Define dimension as L

The is no argument that the beams that delineate the bays are obstructions. 
Even if the spray can throw under it, that doesn't change that consideration.

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: December-21-17 5:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: S & L Rule

I recently learned that the beam only acts like a wall if you can't throw under 
it, so get those deflectors way up there!
(Crow and Thunderbird rocks)

Merry Christmas Forum,

Brad.

Quoting Bob <b...@firebyknight.com>:

> The beam is an obstruction that acts like a wall.  You’re covering 
> floor space, so as long as each sprinkler covers the correct area (30 
> sf), then the spacing that you are describing sounds in compliance 
> with NFPA 13 spacing rules.
>
>
>
> Thank you,
>
>
>
> Bob Knight, CET III
>
> 208-318-3057
>
>
>
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of James Crawford
> Sent: Thursday, December 21, 2017 3:00 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: S & L Rule
>
>
>
> We have been having a discussion in the office about the S rule for 
> spacing of sprinkler heads. We received a sprinkler drawing with some 
> spacing that we do not agree with, see below, but can find no specific 
> direction in NFPA #13 (2013) that says it is wrong.
>
>
>
> Basic situation we have a small building with a 20’ bay and a 30’ bay.
> Ordinary hazard spacing.
>
>
>
> For the 20’ wide bay, we have2  lines spaced at 10’ apart , so we have 5’
> off the wall then 10’ between the next line and 5’ to the beam line, 
> the heads are spaced at 13’ along these lines.
>
>
>
> Then we have a 30’ bay  where we have 2 lines spaced 15’ apart, 7’6 
> off the beam then 15’ between the heads then 7’6 to the wall, heads are 
> spaced at 8’
> along the line
>
>
>
> So our discussion is the sprinkler lines along the beam line which 
> would be 5’-0” plus 7’-6” for 12’-6” between the line. The sprinkler heads in 
> the 20’
> bay are spaced at 13’-0”, so if we use the S rule these heads are 
> spaced at 12’-6” x 13’-0” or 162.6 ft². Is this correct?
>
>
>
> And yes I know we could space the 30’ bay with 3 lines at 10’ apart 
> and that is what I would do but it is not our design.
>
>
>
> Comments
>
>
>
> Thank you
>
>
>
>
>
> James Crawford
>
> Phaser Fire Protection Ltd.
>
> Phone  604-888-0318
>
> Fax 604-888-4732
>
> Cel 604-790-0938
>
> Email  jcrawf...@phaserfire.ca
>
> Web www.phaserfire.ca



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Saw-Tooth Ceilings

2017-11-30 Thread Larry Keeping
With all this talk about spacing, I think maybe the text within NFPA 13 has 
been forgotten. Here's what the standard says on the subject of saw-tooth 
ceilings:

8.6.4.1.3.2*   Under saw-toothed roofs, sprinklers at the highest elevation 
shall not exceed a distance of 36 in. (900 mm) measured down the slope from the 
peak.

A.8.6.4.1.3.2   Saw-toothed roofs have regularly spaced monitors of saw tooth 
shape, with the nearly vertical side glazed and usually arranged for venting. 
Sprinkler placement is limited to a maximum of 3 ft (900 mm) down the slope 
from the peak because of the effect of venting on sprinkler sensitivity.

My advice would be to move the sprinkler to a point 3 ft from the peak. That 
way it will be about 5 ft from the low edge instead of 7 ft, which should 
alleviate the spray/obstruction/spacing problem somewhat.

This is my opinion only and is not intended to represent the NFPA 13 Technical 
Committee, nor serve as an interpretation of the standard.

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: November-30-17 6:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Saw-Tooth Ceilings

I mean, after all, if we can't figure 'half a pattern', how do sidewalls work?
I'm out, because... i, I mean Roland and that face, I mean...
Oh nevermind - - brad..

Quoting bcasterl...@fsc-inc.com:

> Sorry John, wrong side of history on this one.
> Brad.
>
> Quoting John Paulsen <j...@crwnfire.com>:
>
>> I've been watching this thread all afternoon and what I perceived  
>> to be a straight forward question has been complicated beyond  
>> anything I would have thought possible considering the original  
>> question. For me the bottom line here is that if you submit this  
>> layout and hydraulic calculations as anything other than the 14'  
>> dimension on the sloped ceiling, you are going to have to defend it  
>> to the AHJ. Any plan reviewer worth his salt is going to conclude  
>> that the vertical portion of the saw-tooth creates an obstruction  
>> to the spray pattern. That will demand the 7' distance be  
>> considered half the distance the head has to throw to obtain the  
>> correct spacing and design density. If this is OH as previously  
>> stated, in my mind, you are limited to 9' head spacing along the  
>> line.
>>
>> However,
>>
>> If you can get the AHJ and engineer to approve moving the  
>> sprinklers to the middle of the slope and keep the deflector above  
>> 12" from the highest point of the ceiling and in conformance with  
>> Table 8.6.5.1.2 distances from the obstruction, well then you might  
>> have a shot at the 15' head spacing along the line.
>>
>> John Paulsen – SET
>> Crown Fire System Design
>> 6282 Seeds Rd.
>> Grove City, OH 43123
>> P – 614-782-2438
>> F – 614-782-2374
>> C – 614-348-8206
>>
>>
>>
>>
>>
>>
>> -Original Message-
>> From: Sprinklerforum  
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf  
>> Of Michael Hill
>> Sent: Thursday, November 30, 2017 4:26 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: RE: Saw-Tooth Ceilings
>>
>> So you are saying that this is a series of 15 sloped ceilings one  
>> after the other, not a single obstructed saw tooth ceiling.
>>
>> I am not trying to be argumentative. I am trying to convince myself  
>> that what I am being told to do is correct.
>>
>> Mike Hill
>>
>>
>> -Original Message-
>> From: Sprinklerforum  
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf  
>> Of bcasterl...@fsc-inc.com
>> Sent: Thursday, November 30, 2017 4:02 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: Saw-Tooth Ceilings
>>
>> 23.4.4.6 Deisign Densities
>> 23.4.4.6.2, and for backup-
>> 23.4.4.6.5.
>> You don't have walls Michael, you have a sloped ceiling.
>> The down-slope 'half' of the pattern is obstructed, be it sawtooth  
>> or not :).
>> Brad.
>>
>> Quoting Michael Hill <mi...@phoenixfp.net>:
>>
>>> That section explains what to do once the maximum area of protection
>>> is determined. I am still not convinced.
>>> I agree that plenty of water is going to get to the fire, if needed.
>>> More so as this is a UFC project, HC-2 occupancy, dry system,
>>> 0.20/3500.
>>>
>>> Suppose there were walls that extended down to the floor at each end
>>> of the ceiling that created a compartment (which is how I am viewi

RE: [EXTERNAL] RE: Looking for specific sprinkler code on tenant spaces

2017-11-28 Thread Larry Keeping
I’ve been following this thread and so far no one has asked if this would be a 
13 or a 13R application.

I don’t know if it applies, but don’t forget Section 4.5 from NFPA 13R:

4.5   System Arrangement.   In townhouse-style buildings protected in 
accordance with this standard, each dwelling unit shall have its own dedicated 
sprinkler system or the control valve for the sprinkler system in the building 
shall be located outside the dwelling units or in a common area.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark.Phelps
Sent: November-28-17 8:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Looking for specific sprinkler code on tenant spaces

In medical vernacular some surgeons are referred to as having the "God 
syndrome."  If the shoe fits.

Mark at Aero
602 820-7894

Sent from my iPhone

On Nov 28, 2017, at 6:02 PM, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
I was actually taught that term by several fire officials; had never heard it 
in the trade.

SML

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Tuesday, November 28, 2017 4:05 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Looking for specific sprinkler code on tenant spaces

I’ve always called it the “Badge Clause.”  But I like “God Clause” more as some 
that try to apply it this way feel they are God.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Nov 28, 2017, at 4:54 PM, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
I don’t think anybody’s saying it’s a bad idea – I’m certainly in favor of it.  
The question was, is such a requirement in the code (or standard) and the 
answer is no.   So, if an AHJ pulls one out of you-know-where and is asked to 
cite the applicable section, too often they will often cite the section that 
allows local modification by ordinance or regulation, which essentially 
empowers building and fire officials to restrict (or relax) the adopted 
building and fire code.  Its intent is to facilitate local actions, which are 
supposed to be undertaken officially and documented.  It is most assuredly NOT 
the intent of the local modification allowance that an individual gets to just 
make stuff up and force it on us across the counter, but that’s usually how it 
plays when such undocumented requirements are applied.  The response that “I’m 
the fire official and I get to do as I please” has become known derisively as 
the God clause here – don’t know if that’s a universal term or not.

Signed,
Left Coaster

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: Tuesday, November 28, 2017 3:48 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Looking for specific sprinkler code on tenant spaces

God clause? I think it has more to do with trying to keep products of 
combustion from impairing ability to exit the building.

How do they handle near constant T/I’s in malls without tenant shut offs? Still 
assuming a mall.

Best.

Bruce

On Nov 28, 2017, at 15:38, Bruce Verhei 
<bver...@comcast.net<mailto:bver...@comcast.net>> wrote:
Does it meet code definition for a mall? First, is it >50,000 sf.?

A designed active smoke control system may be required. To initiate the smoke 
removal system either smoke detection, zoned by tenant space, or sprinkler 
system water flow, again, zoned by space are allowed.

Of course with addressable detectors smoke detection is in reality a virtual 
zone. This is not the cross zoned system sprinkler folks often run up against.

Smoke removal system is required to be designed by a PE. I would expect their 
activation matrix to include a clear specification as to choice of detection 
method.

I’d also expect a method of testing flow switch.

Provision: I do not have current IFC in front of me.

Opinion. Sprinkler water flow is the way to go. Many fewer unwanted alarms. 
Evacuate the building once for 30 minutes on day after Thanksgiving and they’ll 
never make up any few dollars saved at construction.

Best.

Bruce Verhei

On Nov 28, 2017, at 15:21, Timothy Goins 
<tgo...@rgv.rr.com<mailto:tgo...@rgv.rr.com>> wrote:
I don't know where I read it, but somewhere you must provide at least a common 
room/closet to access the valve and alarm system.. Just in case of an emergency 
or for service. This room must be accessible via outside for the fire 
Department and service personnel. Ore at least that's three plan down here..
And I will give them one 

RE: ESFR Temperature

2017-11-08 Thread Larry Keeping
You are correct, there is nothing in the current edition that references 
radiant heaters.

For the next (2019) edition though, the TC agreed with Public Input No. 555 and 
opted to add "and radiant heater" beside Item (2) Unit heater in the table for 
Temperature Ratings of Sprinklers Based on Distance from Heat Sources (ie Table 
8.3.2.5(a) of the 2016 edition).

In the new standard, with the proposed chapter restricting/reformatting this 
will be Table 9.4.2.5(a).

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: November-08-17 6:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR Temperature

I have a project with Group A plastic storage, We are installing ESFR sprinkler 
to protect the storage per Table 17.2.3.1 (2013). I just found out a bunch of 
radiant heats are going to be installed in the area, and I might need to up the 
temp of the ESFR. Is there a temp. requirement for the ESFR similar to the 
curves in chapter 16-2.1.3.2? I've gone through chapter 17 and can't find it, 
so I wanted to confirm I didn't miss it.

Thanks

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 5 year obstruction testing

2017-10-18 Thread Larry Keeping
I can certainly see the advantage of a camera for obstruction investigations, 
which you would perform if the 5 year assessment of the internal condition of 
piping reveals a problem.

However, for the 5 year assessment itself, all that’s required is to remove 1 
flushing connection cap and 1 branch line fitting and look to see if there is 
any sufficient foreign organic or inorganic material. A camera isn’t needed for 
that, all that’s needed to look inside the pipe ends.   Reference 
NFPA 25, A.14.2.1 (1) (a).

Similarly for the FDC, during normal inspection, all that needed is a look 
through the snoots to see if there is any obstruction in the connection itself. 
A camera shouldn’t be needed for that either.   Reference A.13.8.1 (9).

Larry Keeping



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: October-18-17 4:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 5 year obstruction testing

The Rigid one is handy for FDC connections.
Best

Bruce Verhei

On Oct 18, 2017, at 13:16, Rocci Cetani 3 
<roc...@norcalfire.com<mailto:roc...@norcalfire.com>> wrote:
http://aitproducts.com/mincord.html ($3,700)

ryobi tek 4 also makes one but the camera cord is only a few feet long ($100)

rigid also makes one called the see snake  ($3,500)

there are a bunch out there, just need to google internal pipe cameras

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Lemon
Sent: Wednesday, October 18, 2017 1:07 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: 5 year obstruction testing

Has anyone heard or seen a camera that is used for the 5 year sprinkler 
obstruction testing? Suppose to cut your time in half according to one of my 
field guys. I’ve looked everywhere and haven’t seen what they would be 
referring to.

Thanks


Bill Lemon
Absolute Fire Control, Inc.
215 Lawton Road
Charlotte, North Carolina 28216
(704) 309-5962 Mobile
ble...@absolutefirecontrol.com<mailto:ble...@absolutefirecontrol.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Clean Room Sprinkler Options

2017-10-17 Thread Larry Keeping
I’m no expert on clean rooms or concealed sprinkler’s etc. and while  I think 
the dry sprinkler with the boot is an interesting concept, but I don’t think it 
is meant for that type of application. The brochure for the boot says it is 
intended predominantly for use with clearance holes through freezer ceiling 
structures.

I would advise against using any concealed (or recessed) type sprinklers in a 
clean room, because they are all vented. I understand this is because the heat 
from the fire is supposed to flow through the vents up into the ceiling space. 
Concealed sprinklers have that gap for the cover plate as part of the venting 
configuration.

Even the Reliable “sealing” concealed sprinkler, which seals off the cover 
plate gap is not allowed in ceilings which have positive pressure.

I’ve been told that the reason FM doesn’t sanction Q/R concealed sprinklers is 
because their testing has found that a Q/R concealed sprinkler’s sensitivity is 
roughly equal to a standard response sprinkler installed 12 inches below the 
ceiling. With this, if you interfere with sprinkler’s ability to vent up into 
the ceiling space, as with a boot tight to the cup (ie. with no clearance hole) 
or with insulation all around the sprinkler, you must be even more seriously 
degrading the sensitivity.

If it was up to me I’d use a standard pendant sprinkler in clean room 
applications.

Way-back-when, I did some work at Litton systems and they had a special custom 
fitting/escutcheon with a gasket to make a tight connection to the ceiling, so 
nothing could transfer from the concealed space into the clean room.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: October-17-17 4:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Clean Room Sprinkler Options

If you have a LH or OH criteria where the concealed heads can be used, one 
method that was approved by one of the big insurers for a similar installation 
used the TYCO DSB-2 dry sprinkler boot on the sprinkler drop.  The boot was 
placed over the drop and sealed against the upper side of the celling panel.  
The concealed sprinkler used the gasket option on the room side of the 
sprinkler.

This method according to the underwriter had been proven to stop any 
infiltration into the occupied space from the ceiling cavity.

But if you have an EH occupancy, then that’s another story.

I would highly recommend contacting the owner’s Risk Consultant or Insurance 
Underwriter or EOR for input or approval on any method proposed.

Since this could be a “H” occupancy I do certainly hope there is a qualified 
engineer involved in the project.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, October 17, 2017 3:16 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Clean Room Sprinkler Options [EXTERNAL]

Can anyone please assist with a recommendation for a “clean room” sprinkler 
where the clean rooms are designed to be negative pressure (for compounding 
dangerous drugs).

The concealed sprinkler cut sheets that I’ve looked at online generally say 
that the concealed heads cannot be used in negative pressure rooms (positive 
pressure plenums) and this is the type of room design that we require.  The 
FlexHead cleanroom ceiling sprinkler connection doesn’t appear to be easy to 
clean after installation.

What type of quick response sprinkler could be used in a negative pressure room 
that is readily and easily cleanable?  Users wanted to used concealed 
sprinklers as they thought that the concealed sprinklers would be easy to wipe 
down when necessary, but we don’t want to violate the installation instructions 
on the cut sheets that state that the concealed sprinklers can’t be used with 
positive pressure plenums (negative pressure rooms).

Thanks in advance.

Pete Larrimer
VA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: take off before pump

2017-06-22 Thread Larry Keeping
Feeding the lower level off municipal pressure was a common practice here in 
the Toronto area, years ago. It was kind of mandatory, since the dry pipe 
valves in the parking garage were only rated for 175 psi, as were the 
sprinklers.

In this day and age though with higher working pressure ratings available, 
another option is to use high pressure sprinklers. Some are rated for pressures 
up to 300 psi. Naturally system components have to match.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: June-22-17 10:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: take off before pump

I am looking at a high-rise project that has a fire pump feeding automatic 
standpipes. The AHJ does not want any pressure regulators on the standpipes 
(they want all the pressure they can get) – so the lower floors will be much 
higher than 175 psi.

The city pressure is pretty good also. We were considering feeding the lower 
floors of the sprinkler system with a supply taken off BEFORE the fire pump. 
That way we can feed the lower floors on city pressure, and by the time we run 
out of city pressure, the standpipe pressure will be under 175.

That would allow us to supply the whole building without using any Pressure 
Regulators.

Is there any reason not to do it this way? I have not found any code issues 
with it, but I also don’t hear about this approach very often. Any concerns – 
code or otherwise?

Matt
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Combined Sprinkler/Standpipe Riser Size

2017-05-25 Thread Larry Keeping
I’ve always thought it odd that the standards were rewritten so that there 
would be no exceptions and then so many sections start by saying “Except as 
provided by …”.

In this particular instance, I think 7.6.3 is definitely an “exception” to 
7.6.2. Here is the text from the 2000 edition of NFPA 14, before the deletion 
of the exceptions:

5-6.1   Class I and Class III standpipes shall be at least 4 in. (102 mm) in 
size.

5-6.2   Standpipes that are part of a combined system shall be at least 6 in. 
(152 mm) in size.

Exception:   In fully sprinklered buildings having a combined standpipe system 
that is hydraulically calculated, the minimum standpipe size is 4 in. (102 mm).

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: May-25-17 10:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Combined Sprinkler/Standpipe Riser Size


The standard is re-written so there are no "exceptions."  Combo standpipes can 
be 4" when combined with a system per 13 or 13R.

I hope you are not fighting the same AHJ I did with this.  Because 7.6.3 is not 
called an exception, he requires all combo standpipes to be 6".  I even had 
AFSA provide an informal interpretation stating this.  I had an answer from 
NFPA technical questions stating 4" is acceptable.  I had a committee member 
confirm 4" is acceptable.  The particular AHJ would not budge and said those 
interps were just opinions and he felt they were wrong opinions.

Good luck with this one if you are battling that same AHJ.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 5/25/2017 7:10 AM, Bob wrote:
7.6.3 is not an exception so much as it’s a criteria to be followed.  When the 
building is fully sprinklered per NFPA 13 and the system is hydraulically 
calculated the combined standpipe can be 4”.

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of James Litvak
Sent: Thursday, May 25, 2017 8:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Combined Sprinkler/Standpipe Riser Size

NFPA 14 7.6.2 clearly states that a combined system standpipe rider shall be 
minimum 6". Is 7.6.3 intended to be an exception to 7.6.2? I interpret it to be 
an exception, since otherwise 7.6.3 isn't saying anything different than 7.6.1. 
However, there's no language specifying it as an exception.


James




___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>

Virus-free. 
www.avg.com<http://www.avg.com/email-signature?utm_medium=email_source=link_campaign=sig-email_content=emailclient>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flammable & Combustible storage

2017-05-23 Thread Larry Keeping
For a 1200 ft² warehouse area, I'd be surprized if the Class II and Class IIIB 
liquids are stored in separate piles.

If there is a mix of commodities in a pile, Section 12.6.2.3(1) says that the 
quantity per pile and the max. storage height must be the smallest value. With 
this that would limit the pile height to 10 ft for the metal drums and if the 
totes are mixed into the piles too, that would limit things to just 7 ft.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of James Crawford
Sent: May-23-17 7:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Flammable & Combustible storage

NFPA #30  (2008 ed)

We have a client that has a Liquid warehouse (1,200 ft²) that did not require 
sprinkler protection by code, but did require sprinkler protection by the AHJ 
to get a building permit. The system is an Ordinary hazard group 2 dry system.

They store class II and IIIB liquids in steel drums and Plastic IBC, originally 
storage was on the floor to 4'-0" one drum or tote high.

But as with all thing the company grows and they want to store higher.

Table 12.6.2.2 Quantity Limitations for unprotected Liquid Warehouses will 
allow 10'-0" of class II and 15'-0" of class IIIB

So my understanding is that unprotected is defined as not protected to NFPA 
#30, so based on Table 12.6.2.2 they can store these products to the heights 
noted even thou the area is sprinkled to NFPA #13 Ordinary hazard group 2.

Am I missing something?


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Water curtain for wall opening

2017-05-18 Thread Larry Keeping
You might want to look at FM Data Sheet 1-23. They have scheme for protection 
of wall openings via water spray nozzles protecting both sides of the wall, 
using separate deluge systems.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Micah Davis, SET
Sent: May-18-17 8:25 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Water curtain for wall opening


Todd

I ran into a similar situation at a large food packaging plant.  The protection 
we finally decided on was a small deluge system with heat detectors on both 
sides of the wall.  The heat detectors could be mounted at the ceiling where 
the heat would gather.



Micah Davis

www.dynamicfiredesigns.com<http://www.dynamicfiredesigns.com>




From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com> 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>>
Sent: Thursday, May 18, 2017 6:53 AM
To: Sprinkler Forum
Subject: Water curtain for wall opening

I have been asked to look at a situation in an industrial occupancy where there 
are two garage -door size horizontal openings in a wall. The openings cannot 
realistically be closed, so they are asking about a water curtain. I have a 
couple of questions: First, NFPA 13 discusses water curtains around vertical 
openings but not horizontal, from what i found. Am i missing something?
Second, the ceiling is approximately 12 ft above the top of the openings. The 
sprinklers need to be 12" from the deck max. Will that vertical distance create 
an issue with the water curtain performance.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 20 4.7.7.2

2017-04-06 Thread Larry Keeping
I believe that K-25.2 ESFR sprinkler is listed with a 175 psi max. working 
pressure. With a 50 psi pressure, you are most likely dealing with 30 to 35 ft 
storage in a 40 ft high building, so the sprinkler would be at a max. elevation 
of about 39 ft and the highest churn pressure you could ever be allowed would 
be:

175 psi + 39 ft x 0.433 psi/ft = 191.9 psi.

If there are any sprinklers at lower elevations, under obstructions, etc. then 
even lower max. pressures would be allowed.

Therefore you are not allowed to sustain the 211 psi static under any 
circumstances.

My suggestion is to increase the pipe sizing and decrease the pump pressure 
rating.
Also, there is no rule against it in the standard, but I've always felt it to 
be a poor practice to push towards the 150% of pump flow rating. If the flow 
demand goes past the 120% +/- range, I recommend going to the next available 
rating.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Colin Carew (Cambridge)
Sent: April-06-17 4:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2

140 is the pump rating ,   we sitting at 211 static .   I understand the 
premise ,  4.7.7.2 says I am not allowed to do it .  but the biggest challenge 
is that my system design is 12 heads at 50 psi , K25.2 .  I am just squeaking 
under
Demand . I am not sure what other option I have .

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: April-06-17 4:32 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: NFPA 20 4.7.7.2

Is the 140 psi total pressure or pump rating?

The pressure relief valve comes into play if the combination of supply pressure 
and pump pressure exceeds the allowable system pressure, which for most cases 
is 175 psi.

So if you had fluctuating supply pressures, during a higher than normal 
pressure event, the system could relieve and not damage your downstream, 175 
psi rated system.

Is this a diesel or electric?

How much pressure do you need at these heads?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, April 06, 2017 4:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: NFPA 20 4.7.7.2 [EXTERNAL]

Hi Forum ,

Could someone shed some light on the requirements for 4.7.7.2  .   I have a 
project where the quoted fire pump comes with a Pressure relief valve and waste 
cone .

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to get 
the flow and pressure we need to supply a freezer using LP-46 heads .  I find 
many references to the use of Pressure relief valves being
Used but 4.7.7.2 is  causing me to scratch my head .


Colin





___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 430

2017-04-01 Thread Larry Keeping
Go to NFPA 400.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: March-31-17 11:35 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: NFPA 430

I am looking at a location with CLass 3 oxidizers (pool chemicals). According 
to the NFPA subscription service, the latest version of NFPA 430, which deals 
with this, is 2004. Is there anything more current or has this been merged with 
another document?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Call plates

2017-03-23 Thread Larry Keeping
I’m sorry, I made a typo concerning the referenced section number. It was 
actually Section 3053 of NFPA 13-1986:

3053 … The installer shall properly identify a hydraulically designed automatic 
sprinkler system by a permanent placard, or sign under glass, indicating the 
location, number of sprinklers in the hydraulically designed section, and the 
basis of design (discharge density over design area of discharge, including gpm 
and residual pressure demand at base of riser). Such signs should generally be 
placed at the controlling alarm valve or dry pipe valve, for the system 
containing the hydraulically designed layout.


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: March-23-17 11:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Call plates

The following text was first added to the 1968 edition of NFPA 13:

3038 … The installer shall properly identify a hydraulically designed automatic 
sprinkler system by a permanent placard, or sign under glass, indicating the 
location, number of sprinklers in the hydraulically designed section, and the 
basis of design (discharge density over design area of discharge, including gpm 
and residual pressure demand at base of riser). Such signs should generally be 
placed at the controlling alarm valve or dry pipe valve, for the system 
containing the hydraulically designed layout.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, SET
Sent: March-23-17 5:36 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Call plates

Did you mean calc plates or Hydraulic Design Information Sign?

Found in 1996 ed. 8-5 Hydraulic Design Information Sign but can’t see it in 
1989 ed.  I don’t have anything in between.




Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Thursday, March 23, 2017 4:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Call plates

Anybody know what edition of 13 first required call plates.
--
Sent from Gmail Mobile

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Call plates

2017-03-23 Thread Larry Keeping
The following text was first added to the 1968 edition of NFPA 13:

3038 … The installer shall properly identify a hydraulically designed automatic 
sprinkler system by a permanent placard, or sign under glass, indicating the 
location, number of sprinklers in the hydraulically designed section, and the 
basis of design (discharge density over design area of discharge, including gpm 
and residual pressure demand at base of riser). Such signs should generally be 
placed at the controlling alarm valve or dry pipe valve, for the system 
containing the hydraulically designed layout.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, SET
Sent: March-23-17 5:36 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Call plates

Did you mean calc plates or Hydraulic Design Information Sign?

Found in 1996 ed. 8-5 Hydraulic Design Information Sign but can’t see it in 
1989 ed.  I don’t have anything in between.




Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Thursday, March 23, 2017 4:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Call plates

Anybody know what edition of 13 first required call plates.
--
Sent from Gmail Mobile

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: different k-factors in same area

2017-03-03 Thread Larry Keeping
As per 8.15.23.3 and 8.15.23.3.1, the sprinklers are to be extended above the 
office ceiling a for distance equal to 0.6 times the square root of the design 
area, but a minimum of 24 ft.

To my way of thinking, this means that the density out in the warehouse is to 
be extended over the office that far, which means that the k-factor should be 
the same as that of the warehouse sprinklers.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: March-02-17 2:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: different k-factors in same area

Ok, so I go back to my previous post.

If it's just a suspended ceiling and there no combustibles above, no platforms, 
etc., you should be good with extending the whse roof sprinklers 15 ft beyond 
the half wall into the ceiling space above the office as noted in the NFPA 
excerpt I quoted earlier.

FYI, this is predicated upon the space above the office not being able to be 
used in any way for storage or any fuel fired equipment platforms.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tim Easter
Sent: Thursday, March 02, 2017 9:51 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: different k-factors in same area [EXTERNAL]

What is the height of the warehouse roof/ceiling? 40'
What is the height of the half wall? 28'
What is the height of the office ceiling? 14'
Is the space above the office ceiling walled off from the warehouse? no




Tim Easter, PE
W.W. Gay Fire & Integrated  Systems, Inc.
522 Stockton Street
Jacksonville, FL 32204
Phone: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261




 This electronic message contains information from W. W. Gay Fire 
Protection, Inc., which may be confidential or privileged. The information is 
for use of the individual or the entity named above. If you are not the 
intended recipient, please be aware that any disclosure, copying, distribution 
or use of the contents of this message is prohibited. If you have received this 
electronic transmission in error, please notify us immediately at 
1-904-387-7973.

From: craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com> 
[mailto:craig.pr...@ch2m.com]
Sent: Thursday, March 2, 2017 9:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: different k-factors in same area

Another case of where more info helps drive the answers.

What is the height of the warehouse roof/ceiling?
What is the height of the half wall?
What is the height of the office ceiling?
Is the space above the office ceiling walled off from the warehouse?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tim Easter
Sent: Thursday, March 02, 2017 8:58 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: different k-factors in same area [EXTERNAL]

I have a half-wall that separates an office area from a warehouse area. The 
design is for K factors of 8.0 inside warehouse area, and 5.6 inside office 
area. But since the halfwall doesn't reach the deck the area above the office 
area protected from the ceiling  must have same k-factor as warehouse correct? 
Can anyone point that out in NFPA 13 as a code reference?



Tim Easter, PE
[Description: Description: Description: 
http://www.wwgfp.com/MailLogo.gif]<http://www.wwgfp.com/Brochere.jpg>
522 Stockton Street
Jacksonville, FL 32204
Office: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261





 This electronic message contains information from W. W. Gay Fire 
Protection, Inc., which may be confidential or privileged. The information is 
for use of the individual or the entity named above. If you are not the 
intended recipient, please be aware that any disclosure, copying, distribution 
or use of the contents of this message is prohibited. If you have received this 
electronic transmission in error, please notify us immediately at 
1-904-387-7973.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: RE: Single hydrant flow tests.

2017-03-03 Thread Larry Keeping
Way-back-when, here in Canada the Insurance Advisory Organization published a 
booklet about flow testing. It is the only place I’ve ever seen that discussed 
single hydrant flow testing and it advised that one hydrant testing could be 
used as a check on the other tests or as a test method when less than 750 gpm 
is required or anticipated, but warned that it is not accurate.

Because of this, I’ve always avoided single hydrant tests and only did them 
when the demand would be less than 750 and where there were no other options, 
due to there being only one hydrant available and no other outlets that I could 
use to record static and residual pressures.

Please note, the industry standard is 2 hydrant testing, as per the methodology 
laid out in NFPA 291.

Best regards,

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: March-03-17 10:36 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: RE: Single hydrant flow tests.

Matt,

I always like to witness the flow test whenever I can. I want to make sure they 
are doing it right. We have one company that charges $600 for a test and I end 
up doing it because they have no clue.

My point is that I get hydrant information from contractors a lot of times as 
part of the bid package. I wonder if anyone uses info from the water company 
verifies what they do.



On Mar 3, 2017 at 8:28 AM, mailto:m...@afpsprink.com>> wrote:
Many of the water companies around here will set a time and allow you to come 
out and watch – is it close enough that you can supervise?

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>
Sent: Friday, March 03, 2017 7:08 AM
To: Sprinklerforum
Subject: Single hydrant flow tests.

I recently found a local water company does their flow tests using only single 
hydrants (flow and pressure on the same hydrant). Fortunately I have not done 
very much work there. Who verifies the methodology with a water purveyor when 
they get test results? Obviously not many people in my area as they had to look 
up how to do a 2 hydrant test before we did the new one.
___ Sprinklerforum mailin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: HDPE Plastic Bin Box Storage

2016-12-08 Thread Larry Keeping
If the building is a dedicated warehousing facility, I would disagree. Per the 
definition  (3.9.1.18) for Miscellaneous storage:


-Storage height doesn't exceed 12 ft;

-Is incidental to another occupancy use group (ie. manufacturing or 
assembly);

-Doesn't exceed more than 10 percent of the building area or 4000 ft² 
(372 m²) of the sprinklered area;

-Doesn't exceed 1000 ft² in one pile or area; and

-Is separated from other storage areas by at least 25 ft.

If your truck parts supplier conforms to all of those points, sure Chapter 13 
applies. Otherwise I think you need to go to Chapter 15.

Larry

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: December-08-16 2:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HDPE Plastic Bin Box Storage

Right.

Metal truck parts in these plastic bin containers. Miscellaneous Storage still 
applies.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, December 8, 2016 2:07 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage

When I read your 1st e-mail/question, I thought the subject was relative to a 
truck parts supplier/warehousing operation.
If that is correct and the facility is dedicated to storage, and the Group A 
plastics are being stored at a height greater than 5 feet, I don't think you 
should be using the Miscellaneous Storage design criteria from Chapter 13. 
Shouldn't you be looking at Chapter 15?

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: December-08-16 1:52 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage

Thanks Craig:

These bins are 48" square "folding pallet containers" stacked by two's. There 
is no shelving or racking involved, so as a percentage, there is far less 
plastic than metal.

My thinking is to apply 13.2.1 Group A Plastics - "unexpanded/Expanded" - >5' 
<10' = EH2 (.4 over 2,500)

The existing overhead system will provide .6/2,500 with a 40% safety margin.

Thoughts - Arguments?

Thanks,

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
Sent: Thursday, December 8, 2016 12:05 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage

Their concern is whether or not the plastic bins are being considered, not just 
the stored Class I (metal parts) commodity and it's a valid point if there are 
a considerable amount of bins.  If it's one or two short shelves maybe it's not 
a big issue with a .6 density, but that would be an AHJ and Insurer call.

HDPE falls into the Group A plastics category.

The metal parts are irrelevant to the case.  You have shelves full of plastic 
bins. If the bins were empty how would you classify the storage?

If you look at NFPA 13 (2013) Table 15.2.6(a), for storage >5ft but ≤12ft, 
Roof/Ceiling height at >20 to 32ft (you said system pipe was at 25 ft), the 
density shown is 0.7 gpm/sf for Nonexpanded, stable, exposed.

If in fact your final analysis of the design criteria does show a requirement 
of .7 gpm/sf, I'd calculate the existing systems as-is and see if it can meet 
that criteria.  You might not need to change anything other than prove it works 
as-is.  Then you'd also need to be sure the water supply is adequate for the 
increased flow demand.  The other thing to consider is the NFPA 13 criteria 
only requires calculating of a 2,500 sq. ft. hyd. area, the 3,000 sf area 
sounds like an insurer requirement so you may have some wiggle room there 
hydraulically if you compare the 0.6@3000<mailto:0.6@3000> to 
0.7@2500<mailto:0.7@2500> but you won't know for sure until you run the calc.

I would be looking at the plastics, not the metal parts.



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 11:29 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage [EXTERNAL]

Jeff:

I appreciate your "caution" on this and perhaps I am overreaching here. But in 
my view, I'm just trying to correctly interpret the commo

RE: HDPE Plastic Bin Box Storage

2016-12-08 Thread Larry Keeping
When I read your 1st e-mail/question, I thought the subject was relative to a 
truck parts supplier/warehousing operation.
If that is correct and the facility is dedicated to storage, and the Group A 
plastics are being stored at a height greater than 5 feet, I don't think you 
should be using the Miscellaneous Storage design criteria from Chapter 13. 
Shouldn't you be looking at Chapter 15?

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: December-08-16 1:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HDPE Plastic Bin Box Storage

Thanks Craig:

These bins are 48" square "folding pallet containers" stacked by two's. There 
is no shelving or racking involved, so as a percentage, there is far less 
plastic than metal.

My thinking is to apply 13.2.1 Group A Plastics - "unexpanded/Expanded" - >5' 
<10' = EH2 (.4 over 2,500)

The existing overhead system will provide .6/2,500 with a 40% safety margin.

Thoughts - Arguments?

Thanks,

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
Sent: Thursday, December 8, 2016 12:05 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage

Their concern is whether or not the plastic bins are being considered, not just 
the stored Class I (metal parts) commodity and it's a valid point if there are 
a considerable amount of bins.  If it's one or two short shelves maybe it's not 
a big issue with a .6 density, but that would be an AHJ and Insurer call.

HDPE falls into the Group A plastics category.

The metal parts are irrelevant to the case.  You have shelves full of plastic 
bins. If the bins were empty how would you classify the storage?

If you look at NFPA 13 (2013) Table 15.2.6(a), for storage >5ft but ≤12ft, 
Roof/Ceiling height at >20 to 32ft (you said system pipe was at 25 ft), the 
density shown is 0.7 gpm/sf for Nonexpanded, stable, exposed.

If in fact your final analysis of the design criteria does show a requirement 
of .7 gpm/sf, I'd calculate the existing systems as-is and see if it can meet 
that criteria.  You might not need to change anything other than prove it works 
as-is.  Then you'd also need to be sure the water supply is adequate for the 
increased flow demand.  The other thing to consider is the NFPA 13 criteria 
only requires calculating of a 2,500 sq. ft. hyd. area, the 3,000 sf area 
sounds like an insurer requirement so you may have some wiggle room there 
hydraulically if you compare the 0.6@3000<mailto:0.6@3000> to 
0.7@2500<mailto:0.7@2500> but you won't know for sure until you run the calc.

I would be looking at the plastics, not the metal parts.



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 11:29 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage [EXTERNAL]

Jeff:

I appreciate your "caution" on this and perhaps I am overreaching here. But in 
my view, I'm just trying to correctly interpret the commodity classification 
and arrangement as it relates to the storage provisions of  NFPA-13, which 
should fall under my practice. In fact, I am working with a specifying engineer 
on this who is just as baffled by the insurance underwriter's concerns as I am. 
The problem is, this arrangement is not "specifically" addressed in 13. Is this 
bin box storage, (it's not cardboard or corrugated) or open container storage? 
From everything that I can tell, if it meet the OHII curve, that should be the 
governing requirement.

Thanks,

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Hewitt
Sent: Thursday, December 8, 2016 11:03 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HDPE Plastic Bin Box Storage

John,

I'm writing off on the forum because I don't want to stir up a hornets nest.

Isn't this an engineering decision, not a NICET SET decision?

I'm just saying, why would you want to take that liability as a NICET SET, and 
also potentially violate your NICET Certification by practicing engineering.

Jeff Hewitt, PE, SET, PM.SFPE
Corporate

RE: College Lab Classrooms

2016-12-05 Thread Larry Keeping
I’m surprized no one participating in this thread has mentioned NFPA 45 or its 
extracted text in Section 22.8 of NFPA 13-2016.

If there are chemicals used in the lab in question, the amount needs to be 
determined to enable classification of the space as a Class A, B, C or D type 
lab. Then Class A or B are designated as OH2 occupancies and Class C or D are 
considered OH1.

If there are no chemicals, then you could classify the lab occupancy based on 
the Occupancy definitions.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net
Sent: December-05-16 10:55 AM
To: sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: College Lab Classrooms

Surely you jest.


From: "Brad Casterline" 
<bcasterl...@fsc-inc.com<mailto:bcasterl...@fsc-inc.com>>
To: "sprinklerforum" 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Sent: Monday, December 5, 2016 10:47:57 AM
Subject: RE: College Lab Classrooms

that's easy to answer!
From NFPA 13 (most editions for years):

5.2* Light Hazard Occupancies. Light hazard occupancies shall
be defined as occupancies or portions of other occupancies
where the quantity and/or combustibility of contents is low and
fires with relatively low rates of heat release are expected.
5.3* Ordinary Hazard Occupancies.
5.3.1* Ordinary Hazard (Group 1).
5.3.1.1 Ordinary hazard (Group 1) occupancies shall be defined
as occupancies or portions of other occupancies where
combustibility is low, quantity of combustibles is moderate,
stockpiles of combustibles do not exceed 8 ft (2.4 m), and fires
with moderate rates of heat release are expected.
5.3.1.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.
5.3.2* Ordinary Hazard (Group 2).
5.3.2.1 Ordinary hazard (Group 2) occupancies shall be defined
as occupancies or portions of other occupancies where the
quantity and combustibility of contents are moderate to high,
stockpiles of contents with moderate rates of heat release do not
exceed 12 ft (3.66 m), and stockpiles of contents with high rates
of heat release do not exceed 8 ft (2.4 m).
5.3.2.2 Dedicated and miscellaneous storage shall be protected
in accordance with Chapter 12 and Chapter 13 as applicable.


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net<mailto:wmens...@comcast.net>
Sent: Monday, December 05, 2016 9:36 AM
To: sprinklerforum
Subject: College Lab Classrooms

Quick question.
College Lab classrooms.  Light or Ordinary hazard?


Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786
fax 941-391-6133
wmens...@comcast.net<mailto:wmens...@comcast.net>
www.wfmconsultinginc.com<http://www.wfmconsultinginc.com>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Excessive air leak rate

2016-12-02 Thread Larry Keeping
Hi Mike:

I didn't give a reply before, because I thought it best that the "hands on" 
guys give you their input rather than my more theoretical ideas.

Anyway, since you came up dry with your first query, my answer to the options 
that you presented is that all of them would be examples of excessive air 
leakage.

Of course it depends on the start / stop pressures, but to my mind if the 
compressor comes on more than once a day, there is too much leakage. It depends 
on the type of system too. A low pressure system can't afford as much leakage 
as one with a 40 psi pressure and a 5 or 6 to 1 water/air ratio.

The reason the requirement changed from the NFPA 25 - 2002 edition text of 10 
psi per week to what is in the standard today is because that leak rate (less 
than 1.5 psi per day) is hard to detect during an inspection.

I don't think the idea is to be totally satisfied with a pressure loss as large 
as 36 psi per day, but the test is just for something detectable during an 
annual ITM site visit - 3 psi in 2 hours, which the inspector can measure 
fairly easily during his time on site, in conjunction with the annual trip 
test, etc. Anything less would prove difficult to determine.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: December-02-16 3:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Excessive air leak rate

Since I only received one response, I'll try this one last time.

What do you consider to be an excessive air leak for dry or preaction systems 
or at what point do you go searching for the cause of the leak?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?
Something else?

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

Feel free to email me off line.


Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Henke
Sent: Thursday, December 01, 2016 1:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Excessive air leak rate

What would you consider to be an excessive air leak rate for dry or preaction 
systems?
How many psi per day?

An acceptance test for a new system requires less than 1.5 psi in 24 hours. 
That's pretty tight.

NFPA 25 allows 36 psi in 24 hours for the 3 year test. That seems pretty loose.

It looks like NFPA 25 changed it in 2008 from 10 psi per week, which is 1.5 psi 
per day, to 36 psi per day. That's a pretty drastic change.

Would it help if you were notified that the air leak rate is increasing or 
approaching the maximum allowable rate?

How do you know that you have an excessive air leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?

Kind Regards,

mike

Mike Henke CET
Sprinkler Product Manager
___

[http://www.pottersignal.com/signatures/graphics/logo.jpg]

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936   |   direct: 314-595-6740

mi...@pottersignal.com<mailto:mi...@pottersignal.com>   |   
www.pottersignal.com<http://www.pottersignal.com/>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprikler obstruction.

2016-10-20 Thread Larry Keeping
From the 1984 Technical Committee Reports for Proposal 13-401:

“SUBSTANTIATION Guidance is needed for the placement of standard sprinklers (ie 
non sidewall heads) in relation to their horizontal proximity to walls. Dead 
air spaces in corners can effect a sprinkler’s operation time. The minimum 
clearance for sidewall was used (NFPA 13  4-5.4). A recent installation in a 
300 ft long by 9 ft wide corridor caused this concern when the sprinklers were 
located only 1 in off the wall.”

Larry Keeping
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: October-20-16 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.

What is the reasoning for the 4” minimum space to a wall or duct?
It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.

Art at ATCO Fire



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Sprikler obstruction.

For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.

On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
12x16” Duct is tight to ceiling.
Up right Sprinkler is about 6” from ceiling on exposed pipe.
Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.
Adjacent sprinkler is about 6’-0 away.

Art

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Cesar Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sprikler obstruction.

What size is the duct and what is the distance between the sprinkler and the 
top of duct.


De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Asunto: Re: Sprikler obstruction.

Is the duct below the sprinkler deflector?


On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.
I understand when a new sprinkler is installed it shall be 4” away from a wall.
I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.

Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



[Imagen quitada por el remitente. Avast 
logo]<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>


This email has been checked for viruses by Avast antivirus software.
www.avast.com<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



[Image removed by sender. Avast 
logo]<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>


This email has been checked for viruses by Avast antivirus software.
www.avast.com<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Non-Aspirating Sprinklers listed with specific foam?

2016-09-26 Thread Larry Keeping
NFPA 16 has the following text from the middle portion of A.5.3.1.2:

… In addition to chemical compatibility, one should consider effects on 
proportioning and discharge hardware (many listings and approvals are very 
specific with regard to operating pressures, flow ranges, and materials of 
construction of hardware components). …

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dan Arbel
Sent: September-26-16 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Non-Aspirating Sprinklers listed with specific foam?

Dear Frank

Good Explanation.

However, it does not explain sprinklers should be listed together with Specific 
foam.

You need to purchase the sprinkler and the foam from the same company whist 
normally you would purchase the sprinkler from a company that produce sprinkler 
and foam from foam producer.   This put the Foam Producer that is not 
associated with sprinkler manufacturer at disadvantage.

The listing requirement for sprinkler and foam together is mentioned only in 
NFPA409 .  As I noted I did not find such a requirement in the more specific 
NFPA 11 and 15 (Except for Proportioner and Foam) .FMglobal is implicit 
that it is not required.

Best Regard

Dan Arbel Risk Engineering
T: 972-4-8243337
F: 972-4-8243278
M: 972-52-6611337
Mail: d...@riskmanage.com<mailto:d...@riskmanage.com>
W: www.riskmanage.com<http://www.riskmanage.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Frans Stoop
Sent: Monday, September 26, 2016 6:30 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Non-Aspirating Sprinklers listed with specific foam?

Hello Dan,

Aspirating sprinklers aspirate air and mix it with the incoming premix to 
create foam.
Aspirating sprinklers can create low upto medium expansion foam.

Non-aspirating sprinklers cannot aspirate air and thus cannot mix air with 
premix,
but thanks to the film forming property of AFFF and ARFF there is still another 
mechanism that creates foam.
The premix droplets that leave the sprinkler become small sheets of film while 
beiing thrown away from the sprinkler.
The droplets loose their initial shape because the surface tension of the 
premix is about zero.
However the droplets do not desintegrate because the cohesion of the film 
forming component
in AFFF and ARFF concentrate keeps the molecules together in a thin film.
While slung through the air these small film sheets each catch some air in it 
and become bubbles.
The result is that a lot of the discharged premix reaches the floor as low 
expansion foam.

Obviously this works only with film forming agents, hence the listing for 
specific types of foam.

Kind regards,

ir. Frans Stoop
Sr. Fire Protection Consultant
[riskonet_V2]
Singel 540,
NL-1017AZ Amsterdam
The Netherlands
+316 542 37 642
www.riskonet.com<http://www.riskonet.com/>


At 15:36 26-9-2016, you wrote:
Content-Type: multipart/alternative;
 boundary="=_NextPart_000_0029_01D21814.19C948C0"
Content-Language: en-us

Hello Russell

Thanks for your posting.

Aspirating Sprinkler is listed for Foam Brand?

If not why should non-aspirating sprinkler that is designed and listed as a 
sprinkler, either wet or where the ampule is removed, or dry be listed for any 
foam?

Did you locate any such demand is either NFPA 11 or 15?

Dan

Dan Arbel Risk Engineering
T: 972-4-8243337
F: 972-4-8243278
M: 972-52-6611337
Mail: d...@riskmanage.com<mailto:d...@riskmanage.com>
W: www.riskmanage.com<http://www.riskmanage.com/>

From: Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
On Behalf Of Russell & Carol Gregory
Sent: Monday, September 26, 2016 4:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Non-Aspirating Sprinklers listed with specific foam?

The listing requirement is for the TYPE of Foam NOT the BRAND, so s long as it 
is listed for use with AFFF or ARFF then the Brand shouldn’t matter. This is 
where Mil Spec foams were used so brand wasn’t an issue.

Russell Gregory
Christchurch
New Zealand

From: Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
On Behalf Of Dan Arbel
Sent: Monday, 26 September 2016 12:42 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Ofer Halamish
Subject: Non-Aspirating Sprinklers listed with specific foam?

Dear All,

Should Non-Aspirating Sprinkler be listed with a specific foam?

This is what is required by NFPA 409:

6.2.2 Deluge Foam-Water Sprinkler System Design and Performance.

6.2.2.10 The discharge devices shall have a minimum nominal 6.4 mm (1∕4 in.) 
orifice and shall be listed for use with the particular type of foam 
concentrate to be used in the system.

However, such approval is not required by FM

RE: Noncombustible concealed space

2016-09-14 Thread Larry Keeping
I would offer two points for your consideration:


1.  There was an old formal interpretation that advised that deletion of 
sprinklers above a duct was a question for the AHJ, who could access all of the 
circumstances.

2.  Sprinklers above open grid ceilings need to be in compliance with 
Section 8.15.14.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tim Stone
Sent: September-14-16 10:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Noncombustible concealed space

I have an interesting situation.

Steel and concrete School building. A Corridor runs down the middle on each 
floor about 8' wide, W12 steel I-Beams forming the side at the floor deck 
above, (About 12'-0 Floor to Bottom of deck).
There is a large duct running the length of the Corridor about 7'-6 wide x 24" 
tall. This leaves a gap of about 3" on each side between duct and sheetrock 
partitions. The top of the duct is about 11" below the steel Q-Deck above.
An open metal grid ceiling system is installed 12" - 16" below the duct.

We are installing upright heads 1"-4" below the duct allowing the water to 
spray down through the open grid ceiling.

The question is, do I need to install heads above the duct? There will be no 
way to service or replace these heads and if installed between the duct and the 
wall, the head will not meet the minimum 4" off the wall.
Referencing 2010 ed. 8.15.1.2.1, concealed spaces, I believe I am following the 
intent.

Thank you in advance.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net<mailto:tston...@comcast.net>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Paint spray application

2016-08-08 Thread Larry Keeping
Back to the original question, the only sidewall extra hazard sprinkler that 
I’m aware of is the Reliable Model MBEC-14 Extended Coverage Ordinary & Extra 
Hazard Horizontal Sidewall Sprinklers for Metal Building Applications.

It is a specialty sprinkler, but a spray booth is a type of metal 
building/structure.

I believe FM doesn’t like it for flammable and combustible liquids, so that 
agency wouldn’t accept it in a spray booth, but I think a case could be made 
for using it per NFPA 13 and NFPA 33. I’d run it past the tech. reps at 
Reliable though, before I went too far down the road with it.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: August-08-16 9:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Paint spray application

A large paint booth.

American’s first 787-8 in the paint booth

[Inline image 1]

Paine Field, Everett, WA


On Mon, Aug 8, 2016 at 6:38 PM, Travis Mack, SET 
<tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>> wrote:

I think the point they have all been making is that not everything fits into 
your areas of experience.  Yes, I have seen paint booths in excess of 2000 sq 
ft.  So, the design area per EH2 (.4/2000 with reduction based on use of high 
temp sprinklers) would not encompass the entire area of the paint booth.  
Therefore, your idea of using sprinklers outside of their listing and the 
prescriptives of NFPA 13 could be quite bad judgment.  It could also ruin a 
person financially if it went real bad, not counting other possible scenarios 
that could play out.

This forum is a great educational tool as well as a great way to bounce ideas 
between colleagues.  We have to remember that there are some people new in the 
industry that may see posts by a frequent poster and think he knows more and 
has more experience than he actually does.  They may then take this as the 
correct approach, when it is quite obviously not the correct approach.

By sticking to the guidelines of NFPA 13 where they are very clearly black and 
white, we are best able to defend our actions.  NFPA 13 is not a perfect 
document.  But, it does provide us with definite guidelines and legislated 
criteria we can follow.

If you want to get into performance based design and become the responsible 
engineer of record on the projects you are involved in, then more power to you. 
 However, as most of this board is comprised of those at the technician level - 
including yourself - we do not have that luxury.  As such, we do our best to 
follow the published standards and best practices of the industry.

Back to the original question, I have frequently seen these installed as 
pendent sprinklers in the horizontal position.  I also frequently see them on 
flex hose assemblies to aid in  the inspection process.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 8/8/2016 6:25 PM, Brad Casterline wrote:

I don't know Ron. The closest I have come to that is the foam pop-up nozzles 
for protecting the B2 Stealths at Whitman AFB a couple hours drive from where I 
grew up.
It was pretty harry but the normal stuff surrounding it all was fairly standard.
On Aug 8, 2016 8:14 PM, "rongreenman ." 
<rongreen...@gmail.com<mailto:rongreen...@gmail.com>> wrote:
How about the spray booth for a 747 Brad? Or a B-52?

On Mon, Aug 8, 2016 at 5:38 PM, Brad Casterline 
<bcasterli...@gmail.com<mailto:bcasterli...@gmail.com>> wrote:

Show me a spray booth with forty sprinklers Steve
On Aug 8, 2016 7:36 PM, "Steve Leyton" 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
Sure.  And fires that can be spread by running fuel such as plastics and FCL’s 
(not to mention BLEVE’s) can set off 40 standard response sprinklers in a 
minute.   I can only imagine the sheer volume of responding sprinklers and 
skipping that could occur based on how smooth or bumpy the roof/ceiling 
assembly is if you started wantonly plugging QR control-mode sprinklers into EH 
fires.   (On paper) MDD = .80ADD = .275

My opinion only,
Steve L.



From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Brad Casterline
Sent: Monday, August 08, 2016 5:17 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Paint spray application


Shakey ground is all i have ever known Ken.
I am no more a professional than you are.
THINK MAN!
small spaces with fast fires need the fastest acting sprinklers w

RE: HIGH RISE BUILDING

2016-08-04 Thread Larry Keeping
Great! Now what safety factor is to be applied? What type of joint? What 
corrosion allowance? Are those values for CW, ERW or seamless? etc. etc.

I find it interesting that the old handbook gave you one value and the 
Wheatland info. gave another.

I wouldn’t advise going beyond NFPA prescriptive methods without having a good 
engineering solution (ie. calculations) tucked away in your files.

Larry

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of David Autry
Sent: August-04-16 4:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HIGH RISE BUILDING

I have an old Grinnell Pipe Handbook.

1” Sch. 40 ASTM A53 Grade B, up to 650 degrees has a pressure rating of 
2,847psi, 6” Sch. 40 , 1,143psi.

David Autry

Meininger Fire Protection
2521 West L Street, Suite 5
Lincoln, NE 68522
402.466.2616
402.466.2617 fax
da...@mfp-inc.com<mailto:da...@mfp-inc.com>

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Larry Keeping
Sent: Thursday, August 04, 2016 2:57 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

The 300 psi limit comes from 4.2.3 and 4.24 of NFPA 14-2013 (and has a parallel 
in NFPA 13).

4.2.3   Where steel pipe specified in Table 4.2.1 is used and joined by welding 
as specified in Section 4.4 or by roll-grooved pipe and fittings as specified 
in Section 4.4, the minimum nominal wall thickness for pressures up to 300 psi 
(20.7 bar) shall be in accordance with Schedule 10 for pipe sizes up to 5 in. 
(127 mm), 0.134 in. (3.40 mm) for 6 in. (150 mm) pipe, and 0.188 in. (4.78 mm) 
for 8 in. and 10 in. (203 mm and 254 mm) pipe.

4.2.3.1   …

4.2.4   Where steel pipe specified in Table 4.2.1 is joined by threaded 
fittings as specified in Section 4.4 or by fittings used with pipe having cut 
grooves, the minimum wall thickness shall be in accordance with Schedule 30 
[sizes 8 in. (203 mm) and larger] or Schedule 40 [sizes less than 8 in. (203 
mm)] pipe for pressures up to 300 psi (20.7 bar).

So basically, it layouts what wall thickness you can use for up to 300 psi and 
as I said previously, after that it becomes an engineering effort. If you have 
a pressure zone up to 350 psi or an express riser with even greater pressure, 
you’ve moved beyond the prescriptive allowances.

Larry

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: August-04-16 3:16 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

The specifications from ASTM don’t offer those pressures but testing per 
accepted methods, such as ASME B31.1 do.   There’s a data sheet on Wheatland’s 
website showing working pressures for Schedule 40 and 80 ASTM A53 Grades F and 
B:

http://www.wheatland.com/images/standard-steel-pipe/Working_Pressure_Ratings_081114.pdf

For Grade B, pressures range from 750-650 for 4-8” Sch. 40 and from 1350-1200 
for Sch. 80.

I am curious about the basis for your opinion regarding 300 PSI as some sort of 
a benchmark.  NFPA 14 prescribes a  MWP in standpipes of 350 PSI and there is 
no limit for express mains, except that for which the components are rated 
(note “rated” and not “listed” – this was intentional).The trend in 
tactical firefighting is toward higher pressures – apparatus is for sale right 
now with pumps that produce from 300-1,200 PSI and hose/nozzle combinations 
that will make a multitude of patterns at different flow rates, all the way to 
true fog at ultra-high pressures.   The archaic “comfort zone” approach may not 
be what the design or local responding agency are calling for.

Steve


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, August 04, 2016 8:14 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

I don’t think the various pipe specifications such as ASTM A53 or ASTM A795 
will give you design pressures.

In my opinion, when you move beyond the 300 psi limit, you’ve moved out of the 
prescriptive areas of NFPA 13 & NFPA 14, so selection of the type of pipe and 
the corresponding pipe wall thickness now becomes an engineering effort. The 
usual way to engineer this would be to perform calculations as per ASME B31.1 
or ASME B31.3, to prove that the material chosen can safely retain the 
pressures.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Don Casey
Sent: August-04-16 10:43 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

Search for pipe spec’d to A795

From: Sprinklerforum [mailto:sprinklerforum-bou

RE: HIGH RISE BUILDING

2016-08-04 Thread Larry Keeping
The 300 psi limit comes from 4.2.3 and 4.24 of NFPA 14-2013 (and has a parallel 
in NFPA 13).

4.2.3   Where steel pipe specified in Table 4.2.1 is used and joined by welding 
as specified in Section 4.4 or by roll-grooved pipe and fittings as specified 
in Section 4.4, the minimum nominal wall thickness for pressures up to 300 psi 
(20.7 bar) shall be in accordance with Schedule 10 for pipe sizes up to 5 in. 
(127 mm), 0.134 in. (3.40 mm) for 6 in. (150 mm) pipe, and 0.188 in. (4.78 mm) 
for 8 in. and 10 in. (203 mm and 254 mm) pipe.

4.2.3.1   …

4.2.4   Where steel pipe specified in Table 4.2.1 is joined by threaded 
fittings as specified in Section 4.4 or by fittings used with pipe having cut 
grooves, the minimum wall thickness shall be in accordance with Schedule 30 
[sizes 8 in. (203 mm) and larger] or Schedule 40 [sizes less than 8 in. (203 
mm)] pipe for pressures up to 300 psi (20.7 bar).

So basically, it layouts what wall thickness you can use for up to 300 psi and 
as I said previously, after that it becomes an engineering effort. If you have 
a pressure zone up to 350 psi or an express riser with even greater pressure, 
you’ve moved beyond the prescriptive allowances.

Larry

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: August-04-16 3:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HIGH RISE BUILDING

The specifications from ASTM don’t offer those pressures but testing per 
accepted methods, such as ASME B31.1 do.   There’s a data sheet on Wheatland’s 
website showing working pressures for Schedule 40 and 80 ASTM A53 Grades F and 
B:

http://www.wheatland.com/images/standard-steel-pipe/Working_Pressure_Ratings_081114.pdf

For Grade B, pressures range from 750-650 for 4-8” Sch. 40 and from 1350-1200 
for Sch. 80.

I am curious about the basis for your opinion regarding 300 PSI as some sort of 
a benchmark.  NFPA 14 prescribes a  MWP in standpipes of 350 PSI and there is 
no limit for express mains, except that for which the components are rated 
(note “rated” and not “listed” – this was intentional).The trend in 
tactical firefighting is toward higher pressures – apparatus is for sale right 
now with pumps that produce from 300-1,200 PSI and hose/nozzle combinations 
that will make a multitude of patterns at different flow rates, all the way to 
true fog at ultra-high pressures.   The archaic “comfort zone” approach may not 
be what the design or local responding agency are calling for.

Steve


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, August 04, 2016 8:14 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

I don’t think the various pipe specifications such as ASTM A53 or ASTM A795 
will give you design pressures.

In my opinion, when you move beyond the 300 psi limit, you’ve moved out of the 
prescriptive areas of NFPA 13 & NFPA 14, so selection of the type of pipe and 
the corresponding pipe wall thickness now becomes an engineering effort. The 
usual way to engineer this would be to perform calculations as per ASME B31.1 
or ASME B31.3, to prove that the material chosen can safely retain the 
pressures.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Don Casey
Sent: August-04-16 10:43 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

Search for pipe spec’d to A795

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: 2016/08/04 9:36 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

Thanks Steve,
So if I need to exceed 300PSI, all my valves/fittings…ect before the PRV must 
be listed for the higher pressures. The sprinkler pipe does not have to be 
listed but it must have a working pressure higher than my system pressure.  It 
looks like it has to be ASTM 53B Sch 40 but the piping can be grooved.  I could 
not find any working system pressure charts for Sch 10
Everything sound correct?
Thanks,
Dewayne

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Steve Leyton
Sent: Wednesday, August 03, 2016 10:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

For a standpipe system, show them Table 4.2.1.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:44 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: HIGH RISE BUILDING

So when

RE: HIGH RISE BUILDING

2016-08-04 Thread Larry Keeping
I don’t think the various pipe specifications such as ASTM A53 or ASTM A795 
will give you design pressures.

In my opinion, when you move beyond the 300 psi limit, you’ve moved out of the 
prescriptive areas of NFPA 13 & NFPA 14, so selection of the type of pipe and 
the corresponding pipe wall thickness now becomes an engineering effort. The 
usual way to engineer this would be to perform calculations as per ASME B31.1 
or ASME B31.3, to prove that the material chosen can safely retain the 
pressures.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Don Casey
Sent: August-04-16 10:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HIGH RISE BUILDING

Search for pipe spec’d to A795

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: 2016/08/04 9:36 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

Thanks Steve,
So if I need to exceed 300PSI, all my valves/fittings…ect before the PRV must 
be listed for the higher pressures. The sprinkler pipe does not have to be 
listed but it must have a working pressure higher than my system pressure.  It 
looks like it has to be ASTM 53B Sch 40 but the piping can be grooved.  I could 
not find any working system pressure charts for Sch 10
Everything sound correct?
Thanks,
Dewayne

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Steve Leyton
Sent: Wednesday, August 03, 2016 10:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

For a standpipe system, show them Table 4.2.1.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:44 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: HIGH RISE BUILDING

So when it says "sprinkler pipe maximum working pressure" I can ignore it?  How 
do I get this past the reviewer?

Sent from my iPhone

On Aug 2, 2016, at 7:25 PM, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
Okay, time to go outside the box -schedule 10 and 40 piping isn’t required to 
be listed …   ASTM A53B black steel schedule 40 has is rated for working 
pressures of 430 PSI (4”) and 696 PSI (6”).  And those are with welded joints.  
Vic has what … 700 PSI working pressure for the Style 77 (or something like 
that)?   Far and away the hardest equipment to find is valves that act directly 
on the maximum discharge pressure.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Tuesday, August 02, 2016 5:17 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: HIGH RISE BUILDING

Thanks for the information. What did you do for the 300psi limit on pipe?

Sent from my iPhone

On Aug 2, 2016, at 6:36 PM, Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>> wrote:
We made 360 total head at churn if I recall correctly.  Everything downstream 
UL (USA) listed for fire – had to hunt down check and butterfly valves from 
Victaulic rated for 365.   Here in CA all high-rises have tanks, so PSH of 
about 7’ + pump rating at max churn.   Big pump yes, but not a monster as it 
was only a 750.  We had three or four stairs in the basement and podium levels, 
so designed to a couple of points on the curve.   We’ve done foam underwing 
systems for Navy and Marine Corp hangars with .17/15,000 flowing concurrently 
at the roof with total demand of 4,500-5,000 GPM.   Now THOSE are big pumps.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Tuesday, August 02, 2016 4:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HIGH RISE BUILDING

Must have been one hell of a pump.


There is no height limit in latest editions of NFPA 14.   Standpipes that 
directly supply hose connections are limited to 350 PSI (stay tuned for 2019 
cycle on that one) but there is no height or pressure limit on express mains 
that serve upper zones.   Our firm designed a 545’ single zone system for a 
tower here in San Diego.


The foregoing is my opinion only and is not intended to represent the NFPA 14 
Technical Committee, nor serve as an interpretation of the standard.

Steve L.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler

RE: High Rise Standpipe

2016-08-02 Thread Larry Keeping
This is just my 2 cents worth (in Canadian funds), but this is what NFPA 
14-2013 says on the subject:

5.6.4*   A test connection for testing the waterflow device shall be provided.

A.5.6.4   It is acceptable to utilize a hose valve on the standpipe to test the 
waterflow device as long as the water is dispersed to an acceptable location. 
This could be done with a hose valve on the roof or by using a hose connected 
to a hose valve discharging to a suitable location.

So, my reading of this is "a hose ...  discharging to a suitable location". It 
doesn't say "fire hose", so I think a garden hose should suffice.

Pete Schwab's substantiation when he proposed the new A.5.6.4 text was that "It 
should be allowed to use hose valves versus installing a test connection to 
test the waterflow device."

Best regards,

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Versoi, Michael
Sent: August-02-16 6:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: High Rise Standpipe

The specific information regarding the systems was passed along via a phone 
conversation. I assumed the Standpipe(s) in question were Class III, and posed 
the question as such, but was told they were Class II. There could be 
misinformation provided or interpreted. The question is still the same. Is 
Quarterly/Annual waterflow testing through a garden hose to activate the device 
an acceptable means for Class II system or must the Hand Hose station be 
utilized?
Any input would be appreciated.


Best regards,

Michael Versoi
Fire Sprinkler General Foreman
NICET III

Siemens Industry, Inc.
Building Technologies
22010 SE 51st Street
Issaquah, WA 98029
425.507.4300  Office
1.866.674.2728 Fax
425.281.7313  Mobile
24 hr Dispatch: 800-952-6348


This message and any attachments are solely for the use of intended recipients. 
The information contained herein may include trade secrets, protected health or 
personal information, privileged or otherwise confidential information. 
Unauthorized review, forwarding, printing, copying, distributing, or using such 
information is strictly prohibited and may be unlawful. If you are not an 
intended recipient, you are hereby notified that you received this email in 
error, and that any review, dissemination, distribution or copying of this 
email and any attachment is strictly prohibited. If you have received this 
email in error, please contact the sender and delete the message and any 
attachment from your system. Thank you for your cooperation
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 14 / Remote FDC / Manual Stand-pipes

2016-06-06 Thread Larry Keeping
That being the case, my best suggestion is that you could use the latest 
editions of the standard as clarification of the intent for the requirement in 
the 2010 edition.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: June-06-16 1:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 14 / Remote FDC / Manual Stand-pipes

Unfortunately, I am under 2010 Code.

John Irwin
Sprinkler Construction Manager
Critical System Solutions, LLC
Cell: 813.618.2781
Email:  
jir...@criticalsystemsolutions.com<mailto:jir...@criticalsystemsolutions.com>


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Monday, June 06, 2016 1:04 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: NFPA 14 / Remote FDC / Manual Stand-pipes

I think the guidance you are looking for is in Section 5.9 of NFPA 24-2016:

Section 5.9.1 General states that: "Where the AHJ requires a remote fire 
department connection for systems requiring one by another standard,  fire 
department connection shall be provided as described in Section 5.9."

Section 5.9.3.2.1 says: "Control valves shall be permitted in the system piping 
downstream of the fire department connection piping."

In particular, you might want to look at Figure A.5.9(b), Figure 5.9.3.2.1(a), 
Figure 5.9.3.2.1(b) and Figure A.6.2.2.2.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: June-06-16 11:32 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: NFPA 14 / Remote FDC / Manual Stand-pipes

When using a remote FDC on the underground line or the backflow device, how do 
we get around NFPA 14 2010 6.4.1 "Except for the valve required by 6.3.2, 
shutoff valves shall not be installed between the FDC and the system"?

I have done many yard FDCs on four story hotels over the years and have never 
had this question come up. NFPA 13 has an exception to allow for a remote FDC 
or an FDC tied in to a header, but 14 doesn't seem to have this same exception. 
I should note we have combination standpipes. Standpipes will be manual wet.


John Irwin
Sprinkler Construction Manager

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:  727.209.5126
Cell: 813.618.2781
Email:  
jir...@criticalsystemsolutions.com<mailto:jir...@criticalsystemsolutions.com>

[CSS Logo]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 14 / Remote FDC / Manual Stand-pipes

2016-06-06 Thread Larry Keeping
I think the guidance you are looking for is in Section 5.9 of NFPA 24-2016:

Section 5.9.1 General states that: "Where the AHJ requires a remote fire 
department connection for systems requiring one by another standard,  fire 
department connection shall be provided as described in Section 5.9."

Section 5.9.3.2.1 says: "Control valves shall be permitted in the system piping 
downstream of the fire department connection piping."

In particular, you might want to look at Figure A.5.9(b), Figure 5.9.3.2.1(a), 
Figure 5.9.3.2.1(b) and Figure A.6.2.2.2.

Larry Keeping


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: June-06-16 11:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 14 / Remote FDC / Manual Stand-pipes

When using a remote FDC on the underground line or the backflow device, how do 
we get around NFPA 14 2010 6.4.1 "Except for the valve required by 6.3.2, 
shutoff valves shall not be installed between the FDC and the system"?

I have done many yard FDCs on four story hotels over the years and have never 
had this question come up. NFPA 13 has an exception to allow for a remote FDC 
or an FDC tied in to a header, but 14 doesn't seem to have this same exception. 
I should note we have combination standpipes. Standpipes will be manual wet.


John Irwin
Sprinkler Construction Manager

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122
Fax:  727.209.5126
Cell: 813.618.2781
Email:  
jir...@criticalsystemsolutions.com<mailto:jir...@criticalsystemsolutions.com>

[CSS Logo]

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?

2016-04-28 Thread Larry Keeping
It may be of help if you reference the 2016 edition of NFPA 13. 

There, in Section 8.6.4.1.2(5) the 3 ft limit has been deleted. 

The Committee Statement for that revision was that concrete tees are capable of 
withstanding the heat long enough for sprinklers to activate even when the tees 
are closer than 3 feet on centers.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of svang...@aerofire.com
Sent: April-28-16 5:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 13 (2013) 8.6.4.1.2(5) - why the 3ft minimum?

Forum,

We have concrete tee construction.  Bottom of stems measured from the ceiling 
is 26" down.  Centerline of stems are spaced apart in an every other fashion of 
7', 2'8", 7', 2'8", etc.  Ideally we would like to use NFPA 13 (2013) 
8.6.4.1.2(5) to protect the area so we don't have to add additional 
sprinklers/piping.  However it states this is only applicable for 3ft to 7.5ft 
stem spacing.  Can someone tell me the purpose behind the 3ft minimum 
threshold?  Even though we have some 2'8" sections, do you believe the intent 
of this code was for my situation?  Or do you believe the intent is for 
concrete tee construction where every stem is 3ft or less?  I can see people 
interpreting this passage either way as all stems are spaced away from another 
stem more than 3ft, yet all stems are spaced away from another stem less than 
3ft.

To me, it seems ridiculous that I can have stems with any depth (let's say 
10ft)  and spaced 3'1" apart and the deflector can be located 1" below the 
bottom of the stem (10'1") and branchlines can be spaced 15ft apart.  Yet if 
the same depth stems are spaced 2'11" apart the deflector can't be lower than 
22" below the ceiling and because they are now obstructed, they have to be in 
every pocket.

I appreciate anyone's opinion on my situation and/or knowledge/history of this 
codes development.

Note: As I allude to, I know there are other ways to design this system 
utilizing 22" and beam rule.  I am more looking for the "Why's" or the "You 
missed this blurb" that agrees with your stance .

Thanks,
Sean VG





___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Larry Keeping
Just a bit of an update:

Per NFPA24-2016 & NFPA 13-2016, Section 10.1.4.1

10.1.4.1   Underground piping shall be permitted to extend into the 
building through the slab or wall not more  than 24 in. (600mm). 

A.10.1.4.1   Where nonmetallic underground piping is provided above 
grade or inside a building, the following   should be considered:
(1) Exposure from direct rays of sunlight
(2) Compatibility with chemicals such as floor coatings and 
termiticides/insecticides
(3) Support of piping and appurtenances attached thereto (e.g., 
sprinkler risers, backflow preventers)

Per NFPA 13-2016, Section 24.1.6.1.2:

24.1.6.1.2 Where required due to specific mechanical or environmental 
conditions, the transition piece shall be protected against possible 
damage from corrosive agents, solvent attack, or mechanical damage.

In other words, per the latest editions of the standards, it is now okay to run 
PVC into the building for 2 ft max. So now you shouldn't have worry about 
things such as providing barriers or encasing it in concrete, etc. except under 
special circumstances.
 
Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: March-24-16 2:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC FOR INCOMING SERVICE SUPPLY

The problem with PVC or any non-metallic pipe is that if they are not listed 
for above ground service you may need to transition from the plastic to a 
metallic pipe above the slab.

Check the manufacturer's listing for installation restrictions.

At fire temperatures the plastic could be structurally compromised.  Also if 
there is the potential of a pool fire or exposure to certain chemicals, the 
material can be compromised so typically where we use PVC or HDPE for 
underground service we transition to ductile at the base of the riser and 
extend ductile to the mating flange at 1'-0" above the floor for the connection 
to the aboveground sprinkler system.

NFPA makes some statements as to what is permissible and reasonable for this 
application.  Your conditions may vary so you will need to make the call on 
what material is appropriate above the slab.

>From NFPA 24 2013 Handbook
Commentary A.10.1.1
An often overlooked materials issue is that most nonmetallic underground piping 
brought up through the floor of a building could be vulnerable to fire exposure 
or spills of corrosive liquids. Regardless of material type, a section of 
underground pipe is allowed to extend above the floor level up to a maximum of 
24 in. (600 mm). (See 6.3.1.1.1 in NFPA 13.) The requirement in 24.1.6.1 of 
NFPA 13 provides additional guidance on the transition from underground to 
aboveground piping and the need to protect the transition piece from damage. 
Possible methods for protecting the exposed section of underground pipe are to 
encase it in concrete, provide curbing, or provide a barrier.


NFPA 13 2013 Handbook
6.3.1.1.1* Underground pipe shall be permitted to extend into the building 
through the slab
or wall not more than 24 in. (0.6 m).
Commentary:
This requirement was added in the 2013 edition to provide guidance for the 
specific length of
underground piping that can extend into the building. This requirement 
addresses concerns
that pipe, such as PVC, could be vulnerable to damage after penetration inside 
a building.
However, transition from the underground piping system to the aboveground 
piping in the
building is necessary, so an appropriate length was determined to be 24 in. 
(0.6 m). In instances
where the pipe needs to be protected, such as where ultraviolet light or 
flammable
liquids are present, the short length of PVC pipe is commonly protected by 
encasing the pipe
with concrete.

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Thursday, March 24, 2016 11:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: PVC FOR INCOMING SERVICE SUPPLY

Cesar,
 If I read your inquiry correctly the data you need is most likely in FM 
Global Data Sheet 3-10, in Table 1.  It looks as though they don't make a 
distinction in that data sheet based on the type of occupancy.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> *** On 03/23/2016 5:30 
PM, Cesar Lira wrote:
> Somebody know where can I found in any data sheet or FM section, if I 
> can use a PVC pipe until the incoming supply service for a plant?? Or 
> definitely I

RE: Attachment on a Sidewall Sprinkler

2016-03-02 Thread Larry Keeping
I think what you've got there is a Star sprinkler from the 70's or so, before 
the development of the first residential sprinklers and the fast response link. 

It was early attempt to make a quick response sprinkler. The linkage was a 
standard response but the thing beside it is a squib that (as I understand it) 
is supposed to send an hot electric arc to the link to cause it to melt 
out/actuate quickly.

I only every saw them on one installation and I was once told that handling 
them should be like handling explosives, because an accident with that squib 
could do some harm.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott Holman
Sent: March-02-16 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Attachment on a Sidewall Sprinkler

Hello Forum,

A coworker took a picture of a sidewall sprinkler with a funky attachment on 
it. I'm hoping someone knows what it is because we have been unable to find it 
online.

http://i.imgur.com/ZqsFu39.jpg

Thanks!

Scott Holman
Designer
RLH Fire Protection
4300 Stine Road, Bldg 800
Bakersfield, CA 93313
661.410.1351
shol...@rlhfp.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR duration

2016-02-22 Thread Larry Keeping
I think you've latched on to an error. When the TC discussed moving the 
durations and the hose stream allowances from Chapter 18 to include them in 
Table 12.8.6, I don't remember any discussions about changing the durations.

In the 2013 edition, the only ESFR requirement for a 3 hr. duration was for 
on-tread, on side, and laced tires in open portable steel racks or portable 
palletized racks. All of the other  criteria only called for one hr.

I think when the information was moved, an editing mistake was made. It looks 
to me like someone took the worst case.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dan Arbel
Sent: February-22-16 1:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR duration 

Thank you Craig for your response. 

1.  The ESFR is supposed to operate early enough before the fire gets
its hold within the tires.

2.  FMGlobal did not make any changes. 

3.  I'm not aware of any fire testing justifying a triple duration. 

4.  The last significant test series done with ESFRs I know off is
reported in
http://www.lecaoutchouc.com/images/Partie_publique_ESS/Dossier_N1_Version_an
glaise.pdf

I am still looking for hard evidence 

Dan

Dan Arbel Risk Engineering
T: 972-4-8243337
F: 972-4-8243278
M: 972-52-6611337
Mail: d...@riskmanage.com
W: www.riskmanage.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of craig.pr...@ch2m.com
Sent: Monday, February 22, 2016 7:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR duration 

Because 1-hour for a tire fire does nothing but get things wet.   

Water supplies for firefighting is one area where fire protection engineers 
miss the mark big time.  Too many don't even know about Fire Flow out of the 
IFC.

Had a warehouse storing rubber that burned, it was a 12 hour ground attack, 
municipal supply was woefully insufficient for such an event.  FD had to draft 
from the harbor.  

What we often forget is that sprinklers may be the first responders but behind 
that will be humans who have to actually do the dangerous work of extinguishing 
a larger fire.  When we neglect water supplies and only see what's required in 
NFPA 13, we do them and the owner a great disservice.  

Yes tanks and pumps cost money that may never be recouped, but a total loss is 
pretty hard to overcome as well.  

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Dan Arbel
Sent: Monday, February 22, 2016 11:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Grinnell F991

Dear All,

Anybody knows why NFPA 13- Edition 2016  increased the required duration of
ESFR protection of rubber tires storage from 1 hour (Edition 13) to 3 hours?


Regards
Dan Arbel Risk Engineering
T: 972-4-8243337
F: 972-4-8243278
M: 972-52-6611337
Mail: d...@riskmanage.com
W: www.riskmanage.com



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13, 2013; figure 8.6.5.1.2(c)

2016-01-21 Thread Larry Keeping
You have a good memory Roland.   

I submitted Public Input 289 for the "S" dimension off the wall to be corrected 
to be "½S" and for the "18 in. minimum (No Maximum)" to be revised to "No 
Maximum" and that was accepted by the Committee and published in the 1st Draft 
Report.

Somehow though, when the 2nd Draft Report came out, those changes were lost and 
the original unrevised illustrations were back in there. I notified Matt at 
NFPA about this, but he wasn't able to get it fixed - procedural limitations I 
guess.

I believe that in NFPA 13-2016 Figures 8.6.5.1.2(c) and 8.8.5.1.2(c) and 
8.10.6.1.2(c) were meant to be similar to the new Figures 8.9.5.1.4(c) and 
8.10.7.1.4(c). Maybe we can get it fixed during the next cycle. There should 
probably be a new figure for Section 8.7 as well.

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: January-21-16 2:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13, 2013; figure 8.6.5.1.2(c)

what confused the issue is that you attempted to start a new thread by replying 
to a thread on trailers within a warehouse.  

This is a goofy item that defies logic.  There was something in the FR and/or 
SR reports on this where I thought the 18 inch minimum went away (which then is 
logical).  Will look into AFTER I finish an overdue article (unless you beat me 
to it and tell us - lol)

Roland

  
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jan 21, 2016, at 9:47 AM, T. Silva <silva...@shaw.ca> wrote:
> 
> Trying to understand the logic of this section. If the height from deflector 
> to bottom of obstruction is 18" or over it is not an obstruction, but if the 
> height is less than 18" then it is? 
> 
> This section is also in the 2016 edition. 
> 
> Tony 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Drum Drip Valve Guard

2015-12-16 Thread Larry Keeping
I'm not sure where the serious aspects of this thread left off and the joking 
took over, but if someone tries to automatically drain condensate from a 
system, particularly if there is a QOD involved), the effort could very likely  
lead to a dry pipe valve actuation.

My advice, drum drip or not, would be to never try to drain down a system while 
it is in service. That's just asking for trouble.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: December-16-15 5:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Drum Drip Valve Guard

Edit of my previous response. I would imagine that 0.25 to 0.50 seconds, once 
daily would be adequate. Condensate is not draining so much as being expelled 
by 25-40 psig system air.

B.

> On Dec 16, 2015, at 5:53 AM, Fairchild, Jack <jfairch...@ballinger.com> wrote:
> 
> I like it.  Add some type of flow meter and do remote testing this way as 
> well?
>  
> Jack Fairchild
> 
> 
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> Bruce Verhei
> Sent: Wednesday, December 16, 2015 3:34 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Drum Drip Valve Guard
> 
> Why not drain the water as it collects,  instead of when someone opens the 
> valve. 
> 
> NC solenoid driven valve. 24VDC. 1/8"? Drive off 24v auxiliary power circuit, 
> through NC relay contacts.
> 
> Four wire cable pulled near, and past, all low point drains.
> One wire pair is intelligent circuit, controlled by FACP. Other is the 24VDC 
> auxiliary power circuit, normally powered. Dropped at alarm.
> 
> (Intelligent) relay control module connected to above four wire cable.
> 
> Dry contacts on relay connected to solenoid. (If necessary add 
> capacitive sub-circuit to power initial current spike at solenoid 
> operation.)
> 
> Provide programming option
> to direct all relay contact modules, and by inference, valves, in sequence. 
> 
> Five seconds each round? 
> Five rounds/day? 
> Skew towards warmest time of day in coldest month.
> 
> Orifice, frequency, duration arrived at by experimentation and experience, or 
> stronger powered engineering minds than mine.
> 
> Orifice screened.
> 
> Manual valve provided on horizontal connection on T. Use for initial gross 
> draining of dry system.
> 
> Blow water out it builds up, drip by drip. Never have enough to freeze and 
> break fittings. Correct the problem instead of our colleague in Myrtle Beach 
> ordering 60 x 1" valves each fall. Take the plant maintenance person out of 
> the process.
> 
> Best
> 
> Bruce
> 
>> On Dec 14, 2015, at 2:28 PM, Brad Casterline <bcasterli...@gmail.com> wrote:
>> 
>> Cut the problem in half by using half the valves, and none of those 
>> fighting a losing battle by being closed?
>>> On Dec 14, 2015 4:21 PM, "Charles Thurston" <charl...@mbfsg.com> wrote:
>>> 
>>> Hello Brad,
>>> 
>>> We have enough trouble in this area getting the maint. guy to drain 
>>> the ones with 2 valves they can reach and a hand tight plug in the 
>>> bottom. IF we get 3 days below freezing and then a thaw, we will run
>>> 40-60 freeze break calls on the thaw day.
>>> 
>>> That reminds me I need to place our annual order of 60- 1" valves.
>>> 
>>> Monday, December 14, 2015, 3:43:29 PM, you wrote:
>>> 
>>>> I still say we don't need two 1" globe valvles OR any 2" pipe to 
>>>> make a Drum Drip.
>>>> How about a 1" globe at 7' AFF,  then 6' of 1" down to a 1x1/2 red. 
>>>> with
>>> a
>>>> 1/2" fairly easily removed plug?
>>>> In this way, most would-be tamperers would need a ladder and 
>>>> wrench, and honest workers could use the one valve and one plug to 
>>>> acomplish the same thing the picture of drum drips in 13 do.
>>> 
>>>> Brad
>>>> On Dec 14, 2015 10:40 AM, "Jay Stough" <jaycs7...@gmail.com> wrote:
>>> 
>>>>> AGF has a nice setup.  We recently installed one of their heated 
>>>>> drum
>>> drips
>>>>> where the installing contractor put the drum drip outside.  Go to:
>>>>> http://www.testandrain.com/documents/products.html#collectandrain
>>> 
>>>>> *Jay Stough*
>>>>> NICET IV LAYOUT
>>>>> NICET III ITM
>>> 
>>>>> On Mon, Dec 14, 2015 at 10:37 AM, Gre

RE: working in Canada

2015-11-05 Thread Larry Keeping
Our National and Provincial building and fire codes are very different from 
yours. 
We have a CSA fire alarm installation standard and our own Electrical Safety 
Codes. We don't use NFPA 72 or NFPA 70.  
We do use NFPA 13 however, so things aren't too terribly different for 
sprinklers.

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: November-05-15 12:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: working in Canada

Has or does anyone do any design work in Canada?

Is there anything unique or different than working here in the States?

Licensing, design details, etc?

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: question of procedure

2015-11-04 Thread Larry Keeping
Something like that happened back when I used to work for a sprinkler 
contractor. We were told to leave the system off, but the owner started to put 
stock in his building and they had a bad fire.
Luckily the project manager had issued a letter to say that we'd been 
instructed to leave the system off, so we weren't dragged into any law suits or 
insurance claims.
The lesson from this is to ask what the owner wants and then confirm it in 
writing.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: November-04-15 12:10 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: question of procedure

Say a fire sprinkler system is completed and the 200 psi test has been 
performed and passed.  The building is fully sheet rocked and very near to turn 
over.  Yet, the alarms are not in place.  Do you leave the system with the 
control valves open or closed?

Vandalism where some one opens a 2½" hose valve on the top story of a building 
can lead to a lot of water damage with no alarm to signify flow.  Arson where 
the building burns because the system was left closed since no alarms in place 
can also lead to great damage. It seems like a damned if you do and damned if 
you don't.

Is there any code/standard backing for either situation?  A customer is having 
to deal with one of these issues.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Obstructions Against Walls

2015-10-22 Thread Larry Keeping
I haven't seen any rely to your question, so I'll take a stab.

First, I'm not sure where the 30" obstruction width originated. 

As I understand it, if your obstruction is more than 30" wide you would need a 
sprinkler under it, unless there was at least 18" of clearance from the 
deflector to the top of the obstruction, as illustrated in Figure A.8.6.5.1.2, 
which only came into play in the 2010 edition of NFPA 13.

Possibly, if the obstruction isn't too deep, you can omit the sprinkler below 
if you can comply with Table 8.6.5.1.2 and Figure 8.6.5.1.2(a).

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: October-21-15 3:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Obstructions Against Walls

Where does the maximum 30" dimension come from in figure 8.6.5.1.2(b) (2007)? 
What if you have the exact same scenario that's shown there but the width is 
say 36"? Per code I need to then apply 8.6.5.1.2 & 8.6.5.1.2(a) up to a width 
of 48" correct? After that heads would have to be installed under the 
obstruction right?

Just for giggles 8.6.5.1.2(2) comes in handy but where do you draw the line 
with regard to how far the deflector is above the obstruction when you apply 
it? Would you use the 36" limit from 8.6.4.1.1.3 or is there no limit if heads 
are on both sides of the obstruction?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Monitoring 13D control valves in California

2015-10-05 Thread Larry Keeping
If I've read things correctly the only shutoff to the system is at the BFP 
which serves 5 units. 

Since 13D in Section 6.2.3 says that where more than one dwelling unit are 
served by the same water supply, each unit must have its own individual control 
valve, so I am having trouble seeing the set up described as a 13D system.

It looks like a 13R application to me.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of firs...@aol.com
Sent: October-05-15 1:44 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Monitoring 13D control valves in California 

It appears that both the AHJ and contractor  have made mistakes on this 
project. I am interested in finding out what exactly happened. We should all 
play by the same rules. Im trying to figure out what is correct here according 
to standard, CFC & CBC. Like I said, it looks like a 13R but now they're saying 
its a 13D without DCVA monitoring. 

Sent from my iPhone

> On Oct 5, 2015, at 9:48 AM, Steve Leyton <st...@protectiondesign.com> wrote:
> 
> Are you doing a 3rd party inspection or some sort of risk management/loss 
> prevention analysis?  Why not just call the AHJ or installing contractor and 
> ask for approved basis of design?
> 
> SL
> 
> 
> -Original Message-
> From: Sprinklerforum on behalf of firs...@aol.com
> Sent: Mon 10/5/2015 9:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Monitoring 13D control valves in California
> 
> Hi Steve, thanks for responding. Isn't the CBC more restrictive therefore you 
> can't allow something less? This particular system looks like a 13R but they 
> failed to provide electrical for tamper switches. So now they argue it is a 
> 13D serving a building with 5 townhouse's separated by 1 hour construction. 
> My thinking is since it is 5 units, not one or two family dwelling, the 
> exception for electrical monitoring does not apply. Therefore tampers are 
> required. Am I correct?   
> 
> Sent from my iPhone
> 
>> On Oct 5, 2015, at 8:52 AM, Steve Leyton <st...@protectiondesign.com> wrote:
>> 
>> It's possible the AHJ has accepted these to be of limited area if the 
>> sub-systems serve less than 20 sprinklers.  NFPA offers multiple 
>> solutions for "monitoring", including the locking of valves.  Perhaps
>> the AHJ approved an alternative to electronic supervision.   
>> 
>> Steve L.
>> 
>> 
>> 
>> 
>> 
>> -Original Message-
>> From: Sprinklerforum
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
>> firs...@aol.com
>> Sent: Monday, October 05, 2015 7:38 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Monitoring 13D control valves in California
>> 
>> The California Building Code requires sprinkler control valves to be 
>> electrically monitored. One of the exceptions is One and Two Family 
>> Dwellings, 13D.
>> 
>> What if it is a stand alone 13D system? (2" water meter with one DCVA 
>> to a 2" underground, serving a row of 5 town homes with one hour 
>> separations between units. The 2" underground branches off to each unit.
>> Each unit has it's own flow switch and test valve).
>> 
>> The exception specifically states for one and two family dwellings 
>> because the control valve is before the domestic service so shutting 
>> off the sprinklers shuts off the domestic therefor it is self monitoring.
>> The stand alone serving 5 units does not have this valve arrangement 
>> therefore it would require electric monitoring per CBC.
>> 
>> Am I thinking correctly? According to CBC the two control valves on 
>> the DCVA would need tampers, correct?
>> 
>> Owen Evans
>> 
>> Sent from my iPad
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler
>> .org
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC on Fire Pump

2015-09-25 Thread Larry Keeping
The schematic that you are remembering might be Figure A.4.20.1.2(b) of NFPA 
20-2013, which shows a FDC downstream of all of the control valves and check 
valves associated with the fire pump installation.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: September-25-15 9:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

For some reason I thought I remembered seeing a schematic but apparently not. 
So as long as the FDC ties into the pump discharge downstream of the discharge 
check valve I'm good to go correct?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of etamb...@aerofire.com
Sent: Friday, September 25, 2015 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

13 (2013) 8.17.2.4.8

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Friday, September 25, 2015 6:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC on Fire Pump

Glad its Friday but I must be having a brain cramp. Where does it specify 
where the FDC ties into the pump discharge?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC on Fire Pump

2015-09-25 Thread Larry Keeping
Okay, them take a look at Figure A.5.19.1.2(b) in NFPA 20-2007.

Larry

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: September-25-15 11:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

Sounds nice but I only have the 2007 edition.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Friday, September 25, 2015 10:49 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

The schematic that you are remembering might be Figure A.4.20.1.2(b) of NFPA 
20-2013, which shows a FDC downstream of all of the control valves and check 
valves associated with the fire pump installation.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: September-25-15 9:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

For some reason I thought I remembered seeing a schematic but apparently not. 
So as long as the FDC ties into the pump discharge downstream of the discharge 
check valve I'm good to go correct?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of etamb...@aerofire.com
Sent: Friday, September 25, 2015 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FDC on Fire Pump

13 (2013) 8.17.2.4.8

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Friday, September 25, 2015 6:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC on Fire Pump

Glad its Friday but I must be having a brain cramp. Where does it specify 
where the FDC ties into the pump discharge?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Old valves

2015-09-22 Thread Larry Keeping
From NFPA 13 - 2013:

27.2*   Inactive Sprinkler Systems Abandoned in Place.

27.2.1   Where all or part of an inactive sprinkler system is abandoned in 
place, components including sprinklers, hose valves and hoses, and alarm 
devices shall be removed.

27.2.2   Control valves abandoned in place shall have the operating mechanisms 
removed.

27.2.3   Sprinkler system piping and/or valves abandoned in place shall be 
uniquely identified to differentiate them from active system piping and valves.

A.27.2  It is not intended that the entire system or all components be 
removed. Instead, components such as sprinklers, initiating devices, 
notification appliances, and standpipe hose should be removed to reduce the 
likelihood of relying on inoperable systems or features. Control valves and 
other components that are allowed to be abandoned in place should have 
operating mechanisms removed and be painted a unique color to indicate that 
they are no longer in service.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ed Vining
Sent: September-22-15 2:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Old valves

I think this is debatable. If these are non-required systems, the PA and DP 
valves were removed and the detection and alarms are operable or removed, one 
could make a case for the control valves looking like just any industrial 
valves.

On Tue, Sep 22, 2015 at 10:42 AM, Tom Wellen <twel...@firesprinkler.org>
wrote:

> It may be in NFPA somewhere, but here is the wording in the 2012 
> edition of the IFC:
>
> 901.4.5 Appearance of equipment. Any device that has the physical 
> appearance of life safety or fire protection equipment but that does 
> not perform that life safety or fire protection function shall be prohibited.
>
> Commentary:
>  All required or provided life safety or fire protection related 
> equipment must be continued in use and be maintained to meet the 
> requirements in effect at the time of the original installation. Non 
> required equipment that has been taken out of service or cannot 
> function as intended must be dismantled and removed to prevent 
> creating a false impression of protection.
>
> Simply because a nonrequired system does not meet the current 
> standards is neither cause to require its removal (see Section 901.4), 
> nor a reason to require the system to be upgraded. As long as the 
> system is maintained in the manner in which it was intended when 
> installed, it can be allowed to continue.
>
>
> Tom Wellen
>
>
> > On Sep 22, 2015, at 12:07 PM, Jason Grant <jmg140c...@aol.com> wrote:
> >
> > I have a customer that had another contractor replace 2 system ( a 4"
> dry and a 2 1/2" pre action ) during a building renovation. They left 
> the sprinkler valves in place and and just capped off the head side of 
> the valves and locked out the control valves. Is this a code violation?
> >
> > Jason
> >
> > ___
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 925-787-0465
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Larger circular duct obstructions

2015-09-03 Thread Larry Keeping
You might be interested in some of the new provisions in NFPA 13-2016 that 
relate to this subject:

Types of sprinklers below obstructions:

8.5.5.3.3   Sprinklers installed under obstructions shall be of the 
same type (spray, CMSA, ESFR, residential) as   installed at the ceiling 
except as permitted by 8.5.5.3.3.1. 

8.5.5.3.3.1   Spray sprinklers shall be permitted to be utilized under 
overhead doors.

Sprinklers below round ducts:

8.6.5.3.7   Sprinklers installed under round ducts shall be of the 
intermediate level/rack storage type or  otherwise shielded from the 
discharge of overhead sprinklers.

Obstructions to ESFR Sprinklers:

8.12.5.3.3*  For pipes, conduits, or groups of pipes and conduit to be 
considered individual, they must be  separated from the closest adjacent 
pipe, conduit, cable tray, etc. by a minimum of three times the width of the
obstruction. 

A.8.12.5.3.3 ... Otherwise the pipes and/or conduits would be 
considered as a group when applying the   obstruction criteria of 8.12.5.3.1

Light Hazard Protection with ESFR Sprinklers:

12.6.7.1   ESFR sprinklers designed to meet any criteria in Chapter 12 
or Chapter 14 through Chapter 20  shall be   permitted to protect any of 
the following:

(1)   Light hazard occupancies
(2)   Ordinary hazard occupancies 
(3)   Any storage arrangement in Chapter 13 referencing OH1, OH2, EH1, 
and EH2 design criteria

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Gregg Fontes
Sent: September-03-15 11:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Larger circular duct obstructions

Ken,

So you would installed the ESFR sprinkler directly under the center point of 
the round duct.  (i.e. the 84" diameter duct, the sprinkler would be at 42" 
from the edge at the listed distance below.)  Would a round duct collect enough 
head to set this off???

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Thursday, September 03, 2015 6:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Larger circular duct obstructions

Greg,
 A couple of thoughts come to mind for me.

 First, I would regard the large circular duct as similar to unobstructed 
construction.  The location of the deflector of the sprinklers below the duct 
would have to be as called out in 8.12.4.1.  
So, for those purposes the position below the duct would be driven by the 
k-factor you're using.

 Second, the use of an ESFR system to protect LH/OH occupancies is allowed 
by 12.6.7.1, provided that the original design was per the criteria in chapters 
12 through 20.  I don't think the manufacturers are going to stand behind 
designing ESFR's to meet obstruction rules for standard spray sprinklers. To my 
way of thinking the continuous obstruction rules of 8.12.5.3.1 would still be 
applicable.  I don't agree that it would be possible to eliminate the concern 
over obstructions less than 48" wide, as items (3) and (4) of that section 
suggest 24" is the cutoff width.

  I don't know if that's correct, however those are my initial thoughts.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/>

***
On 09/02/2015 2:18 PM, Gregg Fontes wrote:
> Looking at a building that has ESFR fire sprinkler protection.  Half 
> is being used as open office area.  They are installing circular ducts 
> from 32" to 84" diameter with the top of the duct approximately 36"
> below the ESFR deflector (right below the roof trusses).  In reading
> 8.12.5.3 2013 edition, in most cases if not all, Table 8.12.5.1.1 
> cannot be met, so sprinklers will need to be installed under the 
> ducts.  With the duct being 32" to 84" diameter, where would the fire 
> sprinkler be placed?  Per NFPA 13 is a flat barrier required to be 
> installed under the circular duct? FM give you a guideline, but 13 
> does not.  Owner does not want the ESFR sprinklers change out, so 
> again where would you place the sprinkler and/or is a flat barrier 
> required by NFPA 13?  (With a flat obstruction you can either be under 
> it or within so many inches of the end, but a huge diameter 
> obstruction, is it the edge, center ,etc.?)
>
> Second thought, since this is no longer a storage application, can you 
> apply the standard spray sprinkler obstruction rules?  (This still 
> does not state where to install the sprinkler below the obstruction, 
> but you could eliminate the obstruction less than 48".)
>
> Thanks,
> Gregg Fonte

RE: Mixing EC sprinklers with Std coverage sprinklers

2015-07-07 Thread Larry Keeping
Just as a point of information, I thought I should relate to you the new text 
that will be entered into the forthcoming 2016 edition of NFPA 13:

8.3.3.2Where quick-response sprinklers are installed, all 
sprinklers within a compartment shall be quick-   response unless otherwise 
permitted in 8.3.3.3 , 8.3.3.4 , or 8.3.3.5 . 

8.3.3.3Where there are no listed quick-response sprinklers in the 
temperature range required, standard- response sprinklers shall be 
permitted to be used. 

8.3.3.4The provisions of 8.3.3.2 shall not apply to in-rack 
sprinklers.

8.3.3.5Where a sprinkler carries a listing for both 
standard-response protection and quick-response protection at different 
coverage areas, that sprinkler shall be permitted to be installed within a 
compartment at   the spacing for both the quick-response and 
standard-response listings without any separation between the   areas so 
covered.

8.3.3.6When existing light hazard systems are converted to use 
quick-response or residential sprinklers, allsprinklers in a 
compartment shall be changed.

I think that this will satisfy your concerns - at least in the future.

Best regards

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fairchild, Jack
Sent: July-07-15 1:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Mixing EC sprinklers with Std coverage sprinklers

What Scot said, but the most conservative answer is once an EC head is 
installed with the small spacing it is by nature QR and all heads in the space 
would need to be QR.

Jack Fairchild


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Greg McGahan
Sent: Tuesday, July 07, 2015 10:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Mixing EC sprinklers with Std coverage sprinklers

I lost the original question ...but I think that the AFSA has a recent informal 
interp related to this issue


Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Tue, Jul 7, 2015 at 9:07 AM, å...  eurekaig...@gmail.com wrote:

 Interesting question.  If the activation temperatures are close to the 
 same value, then I would match the RTI of the standdard sprinklers 
 with the imputed RTI of the EC.

 An obvious caveat is if the specifications or engineeering report 
 stipulate the QR in this compartment.

 The NFPA 13 intent, I believe, is to prevent QR sprinklers from 
 activating when they are further away from the fire, in the presence 
 of SR sprinklers when these SR sprinklers are nearer to the fire.

 If the compartment is smaller than the design area,...then the case 
 can be made that the hydraulic design will account for all sprinklers 
 activating, regardless of their intended order of activation (1st 
 ring, 2nd ring, etc.) as manipulated by the RTI of the sprinkler.
 Consider what is to be protected from fire by the different sprinklers 
 and modify your judgment accordingly.

 Scot Deal
 Excelsior Fire/Risk Engineering
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipe design pressure

2015-06-09 Thread Larry Keeping
Here in Canada our National Model Building Code follows NFPA 14 fairly closely 
and requires the 100 psi. However, the total water flow rate is held to just 
500 gpm and in a fully sprinklered building, we are allowed to provide less 
than the 100 psi if the 65/500 can be provided via the FDC.

In Ontario where I am, the Ontario Building Code only asks for 65 psi, again 
with 500 gpm maximum and if sprinklered the pressure is permitted to be less 
than 65 psi if the 65/500 can be provided via the FDC.

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of mphe...@aerofire.com
Sent: June-08-15 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Standpipe design pressure

I have a question for the forum at large, and specifically for the NFPA 14 
Committee Members. For the forum community what is the minimum design pressure 
required for a new class I automatic wet standpipe in your location? I know 
what the un-amended  code  says, but it includes the catch-all qualification 
about the AHJ being consulted for specific needs.  So what I'm looking for is, 
in your region/area;

1- Does the local fire code accept the NFPA14 requirement for 100 psi minimum 
operating pressure at the required flow rate?

2 - Does the local fire code amend the NFPA14 requirement from 100 psi to 
something higher or lower?

3 - Does the local Fire Code Official regulate the NFPA14 requirements without 
having amended the current fire code, ie, require a higher or lower pressure 
than the written code?


Also, from the NFPA 14 committee, any comments on discussions leading up to the 
change from 65psi to 100 psi, and your thoughts on the matter will be 
appreciated.

In addition, related comments from the Fire Fighters among us, on actual 
experience in the heat of the battle, are most welcome.

And lastly, in respect of the Forum Traffic Control officials, please respond 
to me directly off forum at mphe...@aerofire.commailto:mphe...@aerofire.com.

Mark at Aero
602 820-7894

Sent from my iPad
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: CPVC listing grey area

2015-05-20 Thread Larry Keeping
You only mentioned the wood trusses. Will the sheathing/decking also be of 
fire-retardant treated wood? If not, then wouldn't you still have to sprinkler 
the space?

Larry Keeping

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Sean Lockyer
Sent: May-20-15 11:38 AM
To: 'sprinklerfo...@firesprinkler.org'; 'sprinklerforum@lists.firesprinkler.org'
Subject: CPVC listing grey area

I have an interesting question to ask of everyone here. I am being asked to 
install an NFPA  13, non-residential sprinkler system in a small, new building 
that will be constructed with wood. However, the wood trusses will consist of 
fire rated lumber with a flamespread rating of less than 25, which will not 
require sprinkler protection since they would considered to then be 
non-combustible, or at the worst, limited combustible. 

With that being said, could you then install CPVC piping in these concealed 
areas without also having to use the specially listed concealed sprinklers 
(such as the CC1, CC2, HIP, BB1, etc.) heads that Tyco makes ?

Remember, you can only install CPVC in an attic or a combustible concealed 
space if you also use those specially listed heads but if the area is 
technically not combustible I would say that you could use CPVC just like if 
you were using CPVC above an gyp board ceiling in an office for example - if 
you take the listing literally.

What does everyone else think ?


  Sean Lockyer
      Project Designer   4617 Parkbreeze 
Court
  Cell    386-279-1197  Orlando, 
Florida 32808
  slock...@aitlifesafety.com      Phone:  407-816-9101
  www.AITLifeSafety.com   Fax:     
407-816-9104


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Residential design areas per NFPA 13 2007

2015-04-29 Thread Larry Keeping
If I read your message correctly, you are dealing with 2 compartments: a 
bedroom and a living room/kitchen area. 

For the bedroom take its area divided by the number of sprinklers within that 
one room. 

For the living room/kitchen, take its area divided by the sprinklers within it.

Do not add the two areas together.

Larry Keeping


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: April-29-15 5:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Residential design areas per NFPA 13 2007

I am looking at using 11.3.1.2  8.6.2.1.2 in NFPA 13 2007 for calculating my 
systems.  I thought of a question while determining the coverage areas for the 
sprinklers.
Under 11.3.1, we calculate the 4 adjacent sprinklers that create the greatest 
hydraulic demand.
Due to pipe routing my design area consists of a bedroom, and living 
room/kitchen.  I have 1 sprinkler in the bedroom, and 5 sprinklers in the 
living room/ kitchen area for a total of 6.  The total sqft area of the areas 
are 612.86 sqft.  Since I have 6 sprinklers in this area, this gives me 102 
sqft/sprinkler which I default to the minimum required flow per the listing.
Am I correct to divide the total square footage by the total number of heads, 
even though 3 are not flowing?  It seems like I should have been using this 
provision for a while, since it produces lower flows than the SxL method.

Thanks again forum!
Jamie Seidl
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org