Steve,
Make sure you look at the appropriate IFC or NFPA 1 if adopted.
There are storage requirements, MAQ’s, and sprinkler protection schemes based
upon liquid classification and container material and size.
Scott
From: Steve Leyton
Sent: Wednesday, December 20, 2023 1:54 PM
To: Discussion
’ max height. No upholstery whatsoever
but there are some other considerations that prompted a Class IV
classification, hence the density. Or should we have plugged in ESFR because
most furniture warehouses have high levels of exposed expanded plastics?
Steve L.
From: Scott Futrell
…
Steve L.
From: Scott Futrell mailto:sco...@ffcdi.com>>
Sent: Thursday, November 09, 2023 10:19 AM
To: Discussion list on issues relating to automatic fire sprinklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Commodity Classification questio
The fire protection in this building and for this hazard should involve a fire
protection engineer.
There will be lithium batteries, one pound propane tanks, and more.
Early detection and activation, as well as interlocks on equipment, in a very
dusty environment should be considered. If it is
Good morning.
I’ve changed the subject from CPVC to follow up these comments.
NFPA statistics are based on NFIRS reports completed within hours or days of an
event. The statistics do not include any of the failure investigations my
colleagues and I undertake. It takes months to determine the
@comcast.net<mailto:tston...@comcast.net>
From: Scott Futrell mailto:sco...@ffcdi.com>>
Sent: Monday, February 20, 2023 5:34 PM
To: Discussion list on issues relating to automatic fire sprinklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] 18"
All,
I don't have access to my older editions right now.
Can anyone tell me if the 18" clearance between the deflector and the top of
storage was in the 1996 edition of NFPA 13?
Thanks in advance.
Scott
_
SprinklerForum mailing list:
Keep in mind that depending upon the IFC edition that is adopted the IFC used
to have tables that did NOT match NFPA 13. So, if you haven’t, look at the IFC,
too.
Scott
From: Fpdcdesign
Sent: Wednesday, February 1, 2023 11:45 AM
To: Discussion list on issues relating to automatic fire
Tim,
I would not expect NFPA to have any real statistics on this.
ECS and others have performed testing and offer white papers.
OSU is currently testing, but I am not impressed with what they are proposing
or the data they appear to be collecting.
I have seen and investigated failures of
I would suggest you might need to provide the size and length of pipe before
the suction flange, the pump size, and the water flow test information for an
appropriate answer.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Taylor Schumacher
Sent: Friday, August 5, 2022 8:35 AM
Agree, however, I’ve seen it recently in new construction. Either the
mechanical contractor didn’t know what he/she was doing or didn’t care.
You start with the adopted Fire Code, use the Mechanical Code as Allan wrote
and then determine what protection is required.
Scott
Office: (763)
I would not recommend this. It is a sure-fire failure event. The tent has to
remain intact for the life of the structure and if it can fail it will. If any
part of that tent isn't properly sealed or falls apart you have a failure.
Exposed inside. Concealed in the heated space with an insulated
Interesting discussion on this forum.
Steve is utilizing the scientific method that needs to be used to avoid a
Daubert challenge and ensure the proper conclusion, if there is one.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Totally agree. Just checking.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Prahl, Craig/GVL
Sent: Wednesday, January 26, 2022 9:15 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon ; Scott Futrell ;
Mike Hairfield
Subject: RE
You didn't mention what the liquid is. If it is a hazardous material as
recognized by the International Fire Code then the 'empty' container is still
considered full unless completely cleaned.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From:
: Taylor Schumacher
Subject: RE: CPVC Fitting
Seems silly that a threaded female x threaded female fitting in CPVC would even
exist?
Taylor Schumacher
-Original Message-
From: Sprinklerforum On Behalf
Of Scott Futrell via Sprinklerforum
Sent: Tuesday, November 09, 2021 2:18 PM
Just ONE of the reasons this forum is so valuable to the fire protection
industry.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Tom Prymak via Sprinklerforum
Sent: Monday, November 01, 2021 10:05 AM
To:
Mike,
That is an interesting situation and thought.
I would defer to Messer's Hall and Denhardt.
For CMDA sprinklers there are requirements in light and ordinary hazard, but I
don't see specific reference to combustible roof materials for storage and CMDA.
The are limitations for spacing of CMSA
PM
To: sprinklerforum@lists.firesprinkler.org; Scott Futrell
Cc: Aaron Peck ; Andrew Baldwin
; Roberto Alvarez
Subject: Re: NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking
Scott, I can appreciate all of that, but Florida has a state fire code. And we
as life safety professionals (contractors
I can't wait to hear what John and Kevin have to say.
It seems that if the sprinkler system understands the vehicle parked under the
canopy is only there temporarily then it isn't a problem. However, if the
sprinkler system doesn't understand the vehicle is parked temporarily and a
fire starts
and repair mechanic
when I was doing hands-on work, has been that I can't recall ever seeing a
leaky tri-seal fitting in a heated, unheated, or cold storage facility whether
part of a dry or a preaction system.
On Fri, Apr 30, 2021 at 10:47 AM Scott Futrell via Sprinklerforum <
sprinklerfo
I'd sure be interested in hearing more on this subject.
"Listing" only partially answers the question.
Roll groove v. cut groove makes a difference.
If the bottom line is as cheap as possible then you go one route.
If the bottom line is an effective fire sprinkler system for the life of the
There really should be a "Like" button for emails, for this thread on George.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Richard Mote via Sprinklerforum
Sent: Monday, February 15, 2021 11:52 AM
To:
Good morning.
I've looked at the flyer briefly and it certainly is moving in the right
direction.
With record lows in Minneapolis and many other locations that are colder than
-25°F in the northern tier of states I wouldn't do it unless it was a loading
dock or somewhere where water damage
Considering how much corrosion I've observed and documented in wet and dry
systems in schedule 10 in 8-15 years - not MIC - we only specify schedule 40.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Steve Leyton via
Just remember to allow for thermal expansion and contraction. It can get very
ugly if the CPVC is restrained and thermal expansion and contraction has not
been appropriately allowed for. This applies when a building is warm in the
summer during construction and then air conditioning is turned
Great comments. Great information.
1" pipe with cast iron fittings filled with water explodes the side out of the
cast iron ell in 52 minutes at 17⁰F and that piece flies 65 feet when not
confined. I’ve done these experiments outside in winter.
Scott
Office: (763) 425-1001 x 2
Cell:
Many more times than you may have heard about, Craig. For a variety of reasons,
there are more fires that exceed the full design area than you are told about.
I recently spent four days at a fire scene where part of a sprinklered, light
hazard building burned to the ground. That fire exceeded
Yes that is more relevant than 404.3 exception 2.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Travis Mack via Sprinklerforum
Sent: Tuesday, December 01, 2020 1:10 PM
To: sprinklerforum@lists.firesprinkler.org
Cc:
Travis,
It would help to know what edition of the IBC is adopted in the community to
narrow the search. Or do you just want to know in general?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Travis Mack via Sprinklerforum
Don't forget, NFPA 30 and International Fire Code sprinkler/foam system
criteria are not in sync. Fire code rules. Also, you have to look to the fire
code to know what edition of NFPA 30 is enforceable.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From:
As I stated in a previous, related thread, you start with the fire code and
work from there. IIIB's are easier to work with from a fire protection
standpoint, but it may take an engineering solution.
Scott
Office: (763) 425-1001 x2
Cell: (612) 759-5556
-Original Message-
From:
You first start with the Fire Code adopted in the community. The fire code has
requirements for flammable and combustible liquids and also includes fire
protection requirements. You have to start there. The IFC varies from NFPA 30
in some sections. There are maximum allowable quantities (MAQ's)
resprinkler.org/ondemand to
learn more.
On Thu, Sep 24, 2020 at 10:07 PM Scott Futrell via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> 2019:
> 8.2.6.6.5.1
> The disconnecting means for an automatic air compressor shall not be a
> general-use light switch or
2019:
8.2.6.6.5.1
The disconnecting means for an automatic air compressor shall not be a
general-use light switch or a cord-and-plug connected motor.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of Ron Greenman via
NFPA 91: Standard for Exhaust Systems for Air Conveying of Vapors, Gases,
Mists, and Particulate Solids
NFPA 654: Standard for the Prevention of Fire and Dust Explosions from the
Manufacturing, Processing, and Handling of Combustible Particulate Solids
Does that help?
Scott
Office: (763)
What edition?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, October 01, 2019 12:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton
Thank you.
Not what I need for PowerPoint slides, but thanks!
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Travis Allen- Allen Engineering [mailto:tra...@allenfpe.com]
Sent: Wednesday, August 28, 2019 4:33 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell
Subject
Of Ben Young via Sprinklerforum
Sent: Tuesday, August 27, 2019 3:24 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ben Young ; Travis Mack, SET, CFPS, CWBSP, RME-G
; Scott Futrell ; David Williams
; Mitchell, Scott
Subject: Re: N1.85 graph paper
I have one made in cad would that work?
On Tue
Does anyone have an electronic metric/imperial N1.85 graph that they would be
willing to share with me offline?
I need it for hydraulics seminars and all I have are jpegs with one or the
other.
Thanks in advance.
Scott Futrell
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
See below.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: David Williams
Sent: Thursday, August 15, 2019 2:39 PM
To: Scott Futrell ; sprinklerforum@lists.firesprinkler.org
Subject: RE: Attic/Concealed space access to sprinkler heads
Language camp facility. Rural area. Installing
David,
Interesting question. You haven't provided enough information for a thorough
answer.
How big of an attic area?
So you intend to mark the location of every upright sprinkler in the concealed
space on the ceiling below? No one will ever paint that gypsum?
Then cut access for NFPA 25
Good morning.
Does the forum have any Australian sprinkler contractors? SFPE is taking their
Sprinkler Design for Engineers class there and I’d like to discuss sprinkler
system design using AS 2118 versus NFPA 13 with a user.
Please contact me offline.
Thanks in advance.
Scott Futrell
.)
Original message
From: Scott Futrell mailto:sco...@ffcdi.com>>
Date: 10/25/18 4:24 PM (GMT-08:00)
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: High School Weight Room
Exposed, expanded, Group A Plastics and when
Exposed, expanded, Group A Plastics and when put on walls and/or floors, and/or
rolled up, would not be protected adequately by LH.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum On Behalf
Of Ron Greenman
Sent: Thursday, October 25, 2018 9:38 AM
To:
I completely agree with Thomas. You’ll need to include total in storage and
the MAQ’s for IB(?) flammable liquids storage in plastic containers(?).
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of
/>
Fire Sprinklers Saves Lives
On Sep 27, 2018, at 2:04 PM, Scott Futrell mailto:sco...@ffcdi.com> > wrote:
Note that I changed the subject.
I believe I’m offended now, my friend.
SFPE’s Sprinkler Design for Engineers Class is specifically targeting
the
] On
Behalf Of Scott Futrell
Sent: Thursday, September 27, 2018 4:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FPE / SFPE
Note that I changed the subject.
I believe I’m offended now, my friend.
SFPE’s Sprinkler Design for Engineers Class is specifically targeting the
engineers that aren’t
there aren’t that many around to start with.
This class is open to, and attended by PE’s, sprinkler designers, and AHJ’s,
and again, the class teaches them what they should be specifying and reviewing
and how to do it.
Scott Futrell, PE, FSFPE, SET, CWBSD
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
Hmmm…I told others I’d stay out of this, but although it has been met with
great skepticism, please go back to my posts that outlined the proper procedure
for investigating the cause, or just keep doing things and see how that works.
Scott (Ghostbuster)
Office: (763) 425-1001 x2
Cell: (612)
of limitations” have run out sometime in the last 50-plus years?
So what would you gain by determining that was the cause? That’s all I’m trying
to get at.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Friday, September 14, 2018 8:47
...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Friday, September 14, 2018 10:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
Please read thoroughly and carefully all of the emails I posted and don’t start
picking at one aspect.
It can
On Sep 13, 2018, at 6:02 PM, Scott Futrell
mailto:sco...@ffcdi.com>> wrote:
Band-Aid and conceivably a waste of money.
Sprinklers are tested at very high pressures, surges aren’t going to randomly
operate sprinklers.
Should the system have a pressure relief valve, probab
Band-Aid and conceivably a waste of money.
Sprinklers are tested at very high pressures, surges aren’t going to randomly
operate sprinklers.
Should the system have a pressure relief valve, probably yes. Is that the
solution here, most likely, no.
Scott
Office: (763) 425-1001 x2
Cell: (612)
of issues or it just
determine that the head will still activate per spec? These heads do not
actually state UL on them, BTW.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Thursday, September 13, 2018 5:34 PM
To:
sprinklerforum
at the same
elevation as the sprinklers themselves.
Creep is certainly a possibility after forty-six years.
I'd evaluate your other buildings too, or just do the fifty year testing early.
Everything else is shooting the dark...
Scott Futrell
Office: (763) 425-1001 x2
Cell: (612) 759-5556
k, NC 28731
rich...@diboco.com
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile
-Original Message-----
From: Sprinklerforum On Behalf
Of Scott Futrell
Sent: Tuesday, July 03, 2018 10:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Acceptance testing at working pressure
I
I would say so that someone is responsibly in charge of making sure it doesn't
fail. If you put it in service and leave without monitoring the
repairs/changes for some given period of time and a failure occurs water damage
could be extensive. I understand if it fails in two hours and three
ngreen...@gmail.com>
253.576.9700
The Universe is monstrously indifferent to the presence of man. -Werner Herzog,
screenwriter, film director, author, actor and opera director (1942-)
On Sat, Jun 16, 2018 at 7:50 AM Scott Futrell
mailto:sco...@ffcdi.com>> wrote:
As a plan specifier
45-6181
Visit the website<http://www.parsleyconsulting.com/>
On 06/15/2018 8:09 AM, Scott Futrell wrote:
Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 failed,
so it won't be included or required.
I consider this unfortunate, but I'd guess that not everyone on the fo
Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 failed,
so it won't be included or required.
I consider this unfortunate, but I'd guess that not everyone on the forum would
agree.
Scott
Office: (763) 425-1001 x2
Cell: (612) 759-5556
-Original Message-
From:
Seems like a fun research project Brad for a Friday afternoon.
>From the 1955 edition,
621: Open sprinklers may be used to protect special hazards, for protection
against exposures, or in other special locations.
777 (c): Where vertical openings are not protected by standard enclosures,
org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of Scott Futrell
Sent: Friday, March 30, 2018 6:24 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: PVC drain line
Yes, I do think that is the way to go, but it is a sprink
ll piping before the valve is.
R/
Matt
Sent from my Verizon 4G LTE Droid
On Mar 30, 2018 4:10 PM, Scott Futrell
<sco...@ffcdi.com<mailto:sco...@ffcdi.com>> wrote:
I can't see a valve at the end of each line being practical. Then you'd need a
lift to drain them when you wanted to us
Well...
Am I having a Friday afternoon brain fart?
Where does 13 say I can't have a drain line out of other materials, and tie-in
drains don't need valves at the end of every line, right?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum
pvc is ok after the drain valve.
But is that practical?
On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell
<sco...@ffcdi.com<mailto:sco...@ffcdi.com>> wrote:
A Friday afternoon conundrum for the group.
I have a client with corrosion issues in several wet, twenty year old, ESFR,
wa
are
trying to accomplish cost-effectively.
What say ye all?
Scott Futrell
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi
I talked to the FD. They will do a yearly inspection, test the waterflow
switch, no charge and look at sprinklers for corrosion and obstruction. No
other testing recommendations to the owners. I specifically ask about twenty
year testing.
So, if NFPA 25 isn't in play, how does a homeowner
Verhei
> On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote:
>
> Forumites:
>
> Scottsdale has required residential sprinklers since 1985 and those
> residential sprinklers are now more than twenty years old. Is anyone
> performing or recommend
have to test fast
response after twenty years, why wouldn't it apply to residential systems?
Comments, thoughts?
Thanks!
Scott Futrell
Futrell Fire Consulty & Design, Inc.
Office: (763) 425-1001 x2
Cell: (612) 759-5556
___
Sprinklerforum mai
I know you can't do dry gridded, but people do.
So assuming it is wet, yes.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Wednesday, December 20, 2017 4:12 PM
Wet or dry?
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mike Hairfield
Sent: Wednesday, December 20, 2017 4:11 PM
To: Sprinkler Forum
Subject: Corrosion
. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of
The water purveyor may have requirements for location of the BFP relative to
the 200 foot run of pipe.
I would never recommend running more than a few feet of pipe through a building
without a flow switch. Some of my water loss investigations have involved
failures of mains without waterflow
Reed,
I didn’t stay in a Holiday Inn last night, and I don’t pretend to be an
attorney.
I personally don’t think there are many records of pipe schedule systems in
fires that are controlled being evaluated to see if they worked properly when
the loss was small. In other words, a sprinkler
I’ll be blunt Reed. Keep those notes and emails because, in my opinion,
nothing you’ve said relieves you as a professional of your liability if
something goes wrong and you KNOW that system, as you wrote, “does not ‘work’”.
KFI and the owner will have some ‘splainin’ to do (old line from the
It's simple to me Reed.
I would not want the liability if the fire occurred in the pipe schedule system
and that system failed to control the fire, as intended. Knowing that it
doesn't work is where your liability begins, in my opinion.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
It would be easy to hijack the other important thread (calculating remodeling)
with the as-built document problem, but I won't go there.
Have a great weekend everybody.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum
erforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Tuesday, August 15, 2017 12:01 PM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sprinkler Accessibility
Agreed, Matt, but how do you perform the required twenty
Agreed, Matt, but how do you perform the required twenty year testing of QR
sprinklers in a combustible concealed space? Just a question for debate…
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of
Todd,
Glass bulb or fusible link?
I’ve documented 155°F and 165°F sprinklers operating in attics, but I don’t
think I’ve seen a 175°F.
I’ve also documented fusible link, ordinary temperature-rated sprinklers
operating in unconditioned attics.
I’m aware that not all attic sprinkler op’s are
Travis,
Was it better than redrawing walls and grid lines and ceilings or not?
Scott
Office: (763) 425-1001 x2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack
Sent: Wednesday, July 19, 2017 7:18 PM
To:
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: CAD drawings
If it's a plotted PDF and you have access to AutoCAD 2017. Your in luck. 2017
can import plotted PDF files and convert them to DWG format.
-Original Message-
From: Scott Futrell <sco...@ffcdi.com<mailto:sco...@ffc
to as-built the sprinkler systems and standpipes, but it is a very
large facility and redrawing from scratch is not a viable option.
Thanks in advance.
Scott Futrell (aka "This sender failed our fraud detection checks and may not
be who they appear to be. Learn abouut spoofing).
Office: (763) 425
NOVEC 1230 most likely is appropriate. Contact your local Kidde Fenwal
distributor.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Prahl, Craig/GVL
Sent: Tuesday, July 18, 2017 3:07 PM
To:
So as not to hijack the thread…I require flush seal gaskets and have for years.
I have hundreds of photos of schedule 10 pipe corroded away without them. In
twelve years or less.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum
I was involved in an investigation a few years ago and learned that the heat
tracing has a life expectancy of roughly ten years.
That would need to be confirmed for the specific equipment and then
arrangements made for its replacement, if true.
I would not specify that type of system for a
Dang it, I'm still a fraud...
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Thursday, June 01, 2017 9:47 AM
To: sprinklerforum
Reliable, heat producing equipment, electric, propane, or natural gas (steam
too) that can be used to maintain at least 40°F in the room at all times.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum
head correction when applicable.
Karen Lesko
via Newton
Mail<https://cloudmagic.com/k/d/mailapp?ct=pa=9.4.53=6.0.1=email_footer_2>
On Thu, May 25, 2017 at 12:29pm, Scott Futrell
<sco...@ffcdi.com<mailto:sco...@ffcdi.com>> wrote:
Forumites:
I know some of you test pumps freque
Thanks Scot and Byron!
Certainly lends substance to the statement in ‘25’ that results should be
evaluated by qualified individuals.
Be safe.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of å...
hrough 8.3.7.2.9.
Do you correct results?
If so, for engine driven pumps only?
Thanks in advance.
Scott Futrell
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.or
All good comments, but the suggestions so far don't ask the important questions
that I alluded too:
Will the buildings all still have electric power to them or maybe some of them?
Potential ignition sources.
Will the buildings all be locked and secured or will there be access to some
for any
.7.2.1
The fire pump test results shall be evaluated in accordance with 8.3.7.2.2
through 8.3.7.2.9.
Do you correct results?
If so, for engine driven pumps only?
Thanks in advance.
Scott Futrell
Office: (763) 425-1001 x 2
Cell: (612) 75
to be addressed before your
request could be appropriately evaluated.
Scott Futrell
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Foltz, Stuart D CIV USARMY CEERD-CERL (US)
Sent
Travis,
The sprinklers do sometimes operate, too.
These systems can fail to adequately suppress a kitchen fire for a variety of
reasons.
Connection to the sprinkler system should ensure that a flow alarm is
transmitted somewhere. (however, sometimes flow alarms are local only, yes).
If the
Todd,
If this is what Jerry is referring to:
https://www.ladbs.org/docs/default-source/publications/information-bulletins/building-code/water-curtain-in-lieu-of-protected-exterior-openings-ib-p-bc2014-106.pdf?sfvrsn=10
I would be very careful. I don’t see engineering or full-scale testing to
Todd,
I would be very careful. Is this a required separation or occupancy wall and is
it required to be fire-rated? If so, as far as I know there has never been any
full-scale testing of sprinklers as an equivalency to hourly ratings of wall
openings (except for window sprinklers). I know it
Douglas,
The problem appears to be when the two small orifices in the ¾” port are
plugged and water doesn’t flow through the trim to the pressure switch. Check
carefully in systems more than five years old and where corrosion in the dry
pipe system is more evident. You will need to remove the
To any of you that do IT on these dry valves that were manufactured sometime
between 2003 and current (I don't know the exact timeframe yet), we took the
second one apart that has had the two small orifices in the back, in the ¾'
alarm port, plugged. When these are plugged water doesn't flow to