https://dl.dropboxusercontent.com/u/15560791/Project%20Information%20Certificate.docx
[https://dl.dropboxusercontent.com/u/15560791/Project%20Information%20Certificate.docx]
-Travis
Travis E. Allen, PE
Principal
Allen Engineering, PLLC
From: Todd Williams [mailto:fpdcdes...@gmail.com
rforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Wednesday, February 15, 2017 6:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Victaulic IR Fittings
OK. The client that used those said they didn't have to make any adjustments
for the fittings.
Todd G Williams, PE
Fire
m-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd Williams
Sent: Monday, February 13, 2017 10:31 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: Re: Owner Info Certicate
Does anyone actually get those?
rictly
prohibited. If you have received this transmission in error, please immediately
notify us by telephone to arrange for return of the documents.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Wednesday, February 15, 2017 5
I have one client who is trying them out on a project. So far the feedback has
been neutral. At least the takeouts are the same.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT Office:
860-535-2080 Cell: 860-608-4559 [tel:860-608-4559] Fax: 860-553-3553
On Wed, Feb 15, 2017
If only 2 ft, you would need concealed space sprinklers. Use their spacing
requirements
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
Office: 860-535-2080 Cell: 860-608-4559 [tel:860-608-4559] Fax:
860-553-3553
On Tue, Feb 14, 2017 at 8:39 AM, Mark Phillips
Does anyone actually get those?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
Office: 860-535-2080 Cell: 860-608-4559 [tel:860-608-4559] Fax:
860-553-3553
On Mon, Feb 13, 2017 at 11:13 AM, Travis Mack, SET
wrote:
Does anyone have this in a word or
Check the job spec (if there is one) to see if anything special is required.
That could override Code if greater. Already got caught in that.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT Office:
860-535-2080 Cell: 860-608-4559 [tel:860-608-4559] Fax: 860-553-3553
On Tue,
Most of the owners of these facilities have restrictions on what is allowed to
be stored and/or quantities allowed (flammable liquids, quantity of tires,
etc). It is best to be aware of what their restrictions are. The basic
assuption I have used is that the storage within these units meets
This is a quick response and would have to think it out a little, but could you
flow from the hose valves on the standpipes and read a static and residual at
one of the back flow preventer test outlets?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT Office:
860-535-2080
Ask them to have an FPE evaluate the protection requirements for the
occupancy. If this is a design build deal, I wouldn't go near it.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
If it is just feeding on sprinkler, any chance you could replace the pendent
with a dry sidewall fed from the heated space?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
Travis,
I did a bunch of tenenat renovations in a mall a while back and both the
AHJ and FM Global required calculations. The reasoning was that the ceiling
layouts tend to be somewhat extreme (lots of soffits, clouds, etc) and the
number of sprinklers in the remote area could increase.
Todd
large
files to MFP Design via: https://www.hightail.com/u/MFPDesign
[https://www.hightail.com/u/MFPDesign]
Sent from my iPhone
On Dec 12, 2016, at 7:46 AM, Todd Williams < fpdcdes...@gmail.com
[fpdcdes...@gmail.com] > wrote:
Does the definition of small rooms include enclosed stairw
Does the definition of small rooms include enclosed stairways? I am working
on a location with 17' x 8 ft stair enclosures was wondering if I can use a
single sprinkler.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
I have used galvanized pipe and fittings in the past and there have not been
any issues (to my knowledge). Definitely corrosion resistant sprinklers and
hanger material. I wouldn't use exposed CPVC. I think as long as there is no
exposed black steel or brass, you should be good.
Todd G
I would treat it similar to a mezzanine in an industrial or warehouse space
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=ti=9.2.5=10.1.1=email_footer_2]
On Wed, Nov 16, 2016
NFPA 13D allows for exclusion of sprinklers in open attached porches. Does
screening count as an enclosure?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
I see this every once in a while in engineer's specs. Most likely came from the
period when FM had a 20 fps restriction.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
Steve,
The Fire Research Council did a study on boat storage in racks. My guess is
that there is some data in that document.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
prinklerforum-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd Williams
Sent: Monday, October 31, 2016 6:11 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: One weird cross connected system
I was at a location last F
I was at a location last Friday that had one of the strangest systems I
have seen. This is a 3 story office/retail space with underground parking
garages. The upper floors are wet and the garages dry. The sprinkler system
on the upper floor has several connections to feed mechanical equipment
it our website [http://www.parsleyconsulting.com/] On 10/27/2016 8:08
AM, Todd Williams wrote:
Ken,
I brought that up because in NFPA 13, they are called "flexible fittings"
not "flexible drops". My thinking is that FUBAR Fire Protection (or someone
like them) is going to t
Ken,
I brought that up because in NFPA 13, they are called "flexible fittings"
not "flexible drops". My thinking is that FUBAR Fire Protection (or someone
like them) is going to try to claim the since NFPA call them fittings that
they won't have to include them in the calcs.
Todd G Williams,
And that does not apply to flexible fittings
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=ti=9.1.28=9.3.5=email_footer_2]
On Thu, Oct 27, 2016 at 9:43 AM, mphe...@aerofire.com
Most of my thoughts have already been expressed by others, but I will add my
name to the chorus of congratulations and thank you.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=ti=9.1.25=9.3.5=email_footer_2]
On Tue, Oct 18, 2016 at 7:24 PM, Brad Casterline
wrote:
but:
1) you still
It depends. Fuel fired equipment?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=ti=9.1.21=9.3.5=email_footer_2]
On Thu, Oct 13, 2016 at 12:09 PM, James Litvak
ms Inc.
bvssytemsinc.com [http://bvssystemsinc.com/]
From: Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd Williams
Sent: Wednesday, October 12, 2016 10:09 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinkle
inklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Wednesday, October 12, 2016 9:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: FDC on 13R
Single or double?
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=pi=9.1.21=10.0.2=email_footer_2]
On Wed, Oct 12,
Single or double?
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=pi=9.1.21=10.0.2=email_footer_2]
On Wed, Oct 12, 2016 at 8:07 AM, Brian Harris wrote:
Looking for opinions. AHJ wants to swap out a single 1-1/2” FDC on a 13R system
and replace it with a
I am working on a facility where the corridors are sub divided by secured
doors (normally closed - require pass card to open). The areas of these
spaces are around 600 sqft. Could this be considered a small room under the
definition in Chapter 3? The existing sprinklers, in some cases, are 8 to
Loud and clear in the upper right hand corner
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=pi=9.1.9=10.0.2=email_footer_2]
On Tue, Oct 4, 2016 at 8:22 PM, Brad Casterline
wrote:
I don't know if this Forum is working or not Russell.
Somtimes it goes on the
FM has different design categories (HC-1, HC-2, etc). Min hose is 250. No
design area reductions. Their Data Sheets are on line but always best to
talk to a rep
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=pi=9.1.9=10.0.1=email_footer_2]
On Thu, Sep 29, 2016 at 7:13 AM, Dewayne
Why ESFR? What about a regular density/area using K11.2 dry pendents?
The other thing you have to consider is the cost of hanging the system, the
cost of detectors and wiring, the additional pipe sizing due to the 30%
increase in remote area and the additional maintenance required for a DIPA
If I have a sidewall down 4" from the ceiling, what is the minimum soffit I
need below that?
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]___
Sprinklerforum mailing list
Is this considered a mixed use occupancy or is there sufficient fire
separation so it could be treated as 2 separate buildings under the Code?
If it is one building, I think you would have to sprinkler the garage. I
would also question the 2nd floor being 13R and not 13 (using residential
: Sprinklerforum [ mailto:sprinklerforum-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd Williams
Sent: Tuesday, August 30, 2016 6:30 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: Flexheads in small
I have a client that did a 4 sprinkler relocate job in an office and used
Flexheads (no sprinklers added). If the sprinklers were connected with hard
pipe, I would probably not do hydraulic calculations. Given that we have
FHs, should I be doing a full 900 or 1500 sqft calculation?
Todd G
If the FD left a pumper connected to the FDC for the duration of the event,
what density could they get out of the existing system?
Do people in VT actually buy pine trees?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using
In case some Einstein forgets to flush the underground.
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Thu, Aug 25, 2016 at 7:12 PM, rongreenman . wrote:
Why would you need to flush CPVC?
On Thu, Aug 25, 2016 at 8:08
er.org] On
Behalf Of Todd Williams
Sent: Wednesday, August 24, 2016 2:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinklers in mechanical closets on balconies
Is the closet inside or outside of the exterior wall?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, C
Is the closet inside or outside of the exterior wall?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Wed, Aug 24, 2016 at 2:05 PM, John Irwin
There are requirements for separation from sewer lines. Try IPC.
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Tue, Aug 23, 2016 at 8:52 AM, Morey, Mike wrote:
I thoroughly reviewed NFPA 24 and reviewed the applicable
Is there a flame spread rating on the material and/or the contents? Could
this create a concealed fire situation which would bring it to EH2?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
We have a purveyor here in CT who will not allow booster pumps fed from
their mains under any circumstances. They cover around 3 times the
population that yours cover. There is no arguing with them. They can do
pretty much what they want as long as it meets health code and doesn't
restrict
Are there any specific Code or Standard references where sleeves are
required passing through walls? I couldn't find anything in either NFPA 13
or IBC.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
Sprinklers water my garden (at 3am when no one is looking). We install pipes
but people smoke things in pipes.
I've always used pendent sprinklers in duct applications, in spite of their
actual orientation, because they would give the best water distribution.
Sent using CloudMagic Email
I have a client with 2 properties where 13D systems will be installed. Both
will be fed from 13D pump and tank systems. The tanks and the pumps will be
located in out buildings and pipe will be run underground to the main
buildings. They want to put all of the valves, alarms, etc in the pump
Does anyone have good input on conserving water during a hydrant flow test?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
from the chiller unit but do not put in the airflow path
near the fans.
On Fri, Jul 22, 2016 at 6:28 AM, Forest Wilson < forestwilso...@gmail.com >
wrote:
I agree. Maybe move the sprinkler head
On Jul 22, 2016 9:25 AM, "Todd Williams" < fpdcdes...@gmail.com > wrote:
I got a call fr
Easier to figure out by hooking up a hose and see what happens
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Wed, Jul 27, 2016 at 11:01 AM, å...
Is it always filled or would it occasionally be empty?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Mon, Jul 25, 2016 at 1:33 PM, James Crawford
A speedo might be advisable
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Fri, Jul 22, 2016 at 2:21 PM, Forest Wilson
wrote:
Long loose hair is also inadvisable.
In fact the older manufacturer manuals used to
I got a call from someone who has had a problem with a sprinkler in one
specific area accidentally discharging. This has occurred multiple times.
It is in a 0 - 14 degree freezer and is located directly over a chiller
unit. The chiller unit goes in to defrost mode 4x per day. The sprinkler is
Section 11.1.2 permits a higher hazard area within a larger space to be
protected with sprinklers over the hazard and 15 ft beyond. Since nothing
is stated, I assume this can be done with a dry system. Is a 30% increase
in area for the calculation required?
Todd G Williams, PE Fire Protection
Are full flow 2" drain tests required for auxiliary dry valves?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]___
er.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd
Williams
Sent: Thursday, July 14, 2016 8:41 AM
To: sprinklerforum@lists.firesprinkler.org
[sprinklerforum@lists.firesprinkler.org]
Subject: Test header on riser
Is there any requirement to install a test header on a
Is there any requirement to install a test header on a riser without a pump
(In addition to arrangement for full flow FDC test)? I have an engineer
insisting that it is. When I asked for referenced, I get the "you look it
up" response. Just want to be sure before I scream back
Todd G
Contact tech support. Thu should be able to help
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Wed, Jul 13, 2016 at 12:42 PM, Ryan Labrie
wrote:
I am having issues with the AutoSprink settings file I
t want to get into that, because this is a placard thread…
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Friday, July 08, 2016 1:55 PM
To: sprinklerforum@lists.firesprinkl
n test.
Maybe you could add both BOR and Source demands, but I don’t agree with posting
Source data in lieu of BOR.
SL
From: Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org
[sprinklerforum-boun...@lists.firesprinkler.org] ] On Behalf Of Todd Williams
Sent: Fr
I'll ask the unthinkable question, is the BoR demand on the placard worthwhile?
Hydraulic calculations are done back to the effective point of the flow test.
The underground losses, hose demand and sometimes backflow preventer losses are
taken before the BoR. Consequently you cannot compare the
Is there any issues using flex fittings with institutional sprinklers?
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
X http://www.firesprinkler.org
[http://www.firesprinkler.org/]
On Jun 23, 2016, at 7:31 AM, Todd Williams < fpdcdes...@gmail.com
[fpdcdes...@gmail.com] > wrote:
Precisely my thoughts. I'm trying to get them to at least box it.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-5
tected. Speculative buildings with ESFR
sprinklers that now have exposed and expanded group A plastics are a failure
waiting to happen.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd William
er.org] On Behalf Of Todd
Williams
Sent: Thursday, June 23, 2016 8:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: K25 ESFR and plastic storage.
I am working on a location with existing K25 ESFR sprinklers. This is an
existing building where a new client is moving in. The ceiling
I am working on a location with existing K25 ESFR sprinklers. This is an
existing building where a new client is moving in. The ceiling height is
approximately 25 ft and there will be rack storage of plastics (both
expanded and unexpanded) to 20 ft. Looking through the chart in 13, there
are
Mel,
My first answer was concrete blocks or quarried stone. Matt is correct in
what he said. In all likelihood, they would have to install a flat ceiling
over the storage because of the 3:12 pitch. Then it becomes a matter of
height, arrangement and material. That water supply is modest at
I have a flow graph program on Excel that you could use and read to 20 psi. It
doesn't have any capacity for calculating underground data
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Thu, May 19, 2016 at 8:55 AM, Brian Harris
:46 PM, rongreenman . <rongreen...@gmail.com>
wrote:
Typically a valve at the rider. Are you looking for the manual release for
a particular riser or a rule as to where it has to be?
On Monday, May 9, 2016, Todd Williams <fpdcdes...@gmail.com> wrote:
> ANy information on locat
t;
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org <javascript:;>] On Behalf
> Of Todd Williams
> Sent: Monday, May 09, 2016 2:33 PM
> To: sprinklerforum@lists.firesprinkler.org <javascript:;>
&g
I'm looking for guidelines for manual pull stations on pre-action systems.
Any idea where they are?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
Worst case scenario
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Mon, May 2, 2016 at 11:04 AM, John Milligan wrote:
Hello
This
Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016
ct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 2:44 PM
To: sprinklerforum@lists.firesprinkler.org
ce out from the
riser).
So the big question is where’s the beef?
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>
> On Apr 27, 2016, at 3:27 AM, Todd Williams <fpdc
sage-
> From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd
Williams
> Sent: Wednesday, April 27, 2016 8:20 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Existing pipe schedule and storage
>
> The original building was built in 188
Behalf Of Todd
Williams
Sent: Wednesday, April 27, 2016 5:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Existing pipe schedule and storage
I am working at a facility where there is an existing OH pipe schedule
system over 12ft palletized Class IV storage. The fire department has
ap
Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, April 27, 2016 6:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Existing pipe schedule and storage
I am working at a facility where there is an
I am working at a facility where there is an existing OH pipe schedule
system over 12ft palletized Class IV storage. The fire department has
approved it, but I question whether it will provide adequate protection. I
did not see anything in NFPA 13 that requires storage occupancies to be
Is it a local/state code requirement. RI used to have a requirement that
the sprinkler zone match the alarm zone, s there were a lot of 20k sqft
sprinkler zones
Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pi=7.4.8=9.2.1=email_footer_2]
On Wed, Apr 13, 2016 at 2:20 PM,
In 2010, 23.1.1: "Number of Supplies. Every automatic sprinkler system
shall have at least one automatic water supply"
However, I did not see anything (admittedly quick review) that says that
sprinklers shall be installed on a piping network (thus creating a
"system"). It does say install per
Is there a rational explanation why the sprinkler contractor should bring
in the last piece of underground from 5 ft outside the building?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
If you remember, a couple of weeks back I posted a question regarding a
pipe schedule system in a building from 1884. I went up this morning and
mapped out the systems. As best I can figure, the pipe schedule goes
something like this:
3/4" - 1 sprinkler 1" - 3 1-1/4" - 6 1-1/2" - 10 2" - 21
I've had very good luck with HP, but I am not doing anywhere near the
volume. You are working on print shop quantities so that puts it in a
different league.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
gt; What is the sprinkler spacing?
> Staggered spacing was quite common before 1940.
> Newer heads installed?
> High pressure water supply connected?
> It likely will barely do .10 density or maybe .15 with moderate
pressure.
> FM used to allow 3-5 psi at end head for pipe schedule.
&
I am working on a project in a mill that was constructed in 1884. On the
top floor, the branch piping is 3/4 - 1 - 1. Was there an older version of
pipe schedule that allowed smaller pipe or is this just undersized?
Hopefully some of you history buffs (or at least those with a bunch of old
I am working with a facility that makes envelopes and other office paper
products. They have an exhaust duct system which feeds twin collectors
outside.
The collectors have built in sprinklers and 1" outlets to connect to. The
owner
wants to connect to the sprinklers in the collector, but a
CT requires either a PE stamp or designer's stamp (state issued
certification
with a NICET III or IV requirement) on all sprinkler drawings, regardless
of
criteria. Consequently, I have stamped 13D systems. It is overkill if you
are
dealing with experienced and ethical designers. Otherwise,
IBC 2009 and beyond have incorporated at least some reference standard for
pool
suction safety, if not specific language.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
74102
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Todd Williams
Sent: Monday, March 07, 2016 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pool as Firewater Source
You migh
You might have a health code issue with that. How could you prevent someone
from
getting stuck in a suction line? There are strict requirements as far as
pool
recirculating drains and I am not sure you could meet those with a fire
pump
suction line. That could create a huge liability problem. I
I did one of these about 10 years ago a nuke plant. The building was a
pre-fab
metal building with the reinforced concrete shooting range inside. We
protected
the entire building but did not have anything inside the range itself.
Todd G Williams, PE Fire Protection Design/Consulting
Was that the gunpowder attached to the barrel of water?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Wed, Mar 2, 2016 at 6:47 PM, Roland Huggins
https://www.hightail.com/u/MFPDesign
On 2/23/2016 1:53 PM, Todd Williams wrote:
> May we assume they are not doing the weekly tests?
>
> Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
> 860-535-2080 (ofc) 860-608-4559 (cell)
> Sent using CloudMagic
> [https://cl
May we assume they are not doing the weekly tests?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Tue, Feb 23, 2016 at 3:31 PM, Travis Mack, SET
There was a tire storage fire in CT last year and they used 2 million
gallons of
water. 3 hour duration is more reasonable than 1 hour
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
ver...@comcast.net> wrote:
Wales.
Todd
Please tell me this isn't autocorrect striking again. I got a good chuckle
and
credited you.
bv
> On Feb 22, 2016, at 08:14, Todd Williams <fpdcdes...@gmail.com> wrote:
>
> If all Wales fails, Tyco should have a copy
>
> Todd G W