RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread BRUCE VERHEI via Sprinklerforum
com | www.jacobs.com > 1041 East Butler Road Greenville, South Carolina 29606 > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Tuesday, August 25, 2020 10:29 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Jo

Re: Window Sprinklers

2020-08-25 Thread AKS-Gmail-IMAP via Sprinklerforum
If you are referring to Tyco WS sprinklers, then you do see that it is not listed when there is a horizontal mullion but you also see in its installation details that there is no maximum distance indicated for the “ceiling” to the sprinkler. Yup, go look at. One other aspect to this is that ther

Re: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Joe Burtell via Sprinklerforum
.com | www.jacobs.com > 1041 East Butler Road Greenville, South Carolina 29606 > > -Original Message- > From: Sprinklerforum On > Behalf Of Joe Burtell via Sprinklerforum > Sent: Tuesday, August 25, 2020 10:26 AM > To: å... > Cc: Joe Burtell ; > spri

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
ast Butler Road Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On Behalf Of John Denhardt via Sprinklerforum Sent: Tuesday, August 25, 2020 10:29 AM To: sprinklerforum@lists.firesprinkler.org Cc: John Denhardt Subject: [EXTERNAL] Re: Window Sprinklers Agre

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
s.com 1041 East Butler Road Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On Behalf Of Joe Burtell via Sprinklerforum Sent: Tuesday, August 25, 2020 10:26 AM To: å... Cc: Joe Burtell ; sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Re: Window Spri

Re: Window Sprinklers

2020-08-25 Thread John Denhardt via Sprinklerforum
Agree 100%. Follow the Listing - period. If an architect or an engineer wants to violate the Listing, let them provide direction and assume all liability. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-

Re: Window Sprinklers

2020-08-25 Thread Joe Burtell via Sprinklerforum
Here is how I see it. All manufacturers prohibit horizontal mullions. My guess is they failed testing when horizontal millions were present. The building code requires the windows to be protected with listed sprinklers. Even if I did put the additional window sprinkler below the horizontal million

RE: Window Sprinklers

2020-08-25 Thread Matt Grise via Sprinklerforum
I would ask - what would the lower sprinklers do? It seems like higher level sprinklers would go off first and then prevent the lower ones from operating. As you mentioned, they are not listed for that application. I have had the discussion before: If you want a fire rating, and a window, you

RE: Window sprinklers

2013-02-22 Thread bcasterline
pth of the mullions to any consideration. Tony -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fairchild, Jack Sent: February 22, 2013 7:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers

RE: Window sprinklers

2013-02-22 Thread A.P.Silva
h of the mullions to any consideration. Tony -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fairchild, Jack Sent: February 22, 2013 7:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers The ICC p

RE: Window sprinklers

2013-02-22 Thread Fairchild, Jack
Subject: Re: Window sprinklers >From what I understand Tyco was not invited to the hearings for the proposed >changes and the rug was pulled out from under them in regard to the Tyco WS >sprinkler for 1hr and 2hr equivalency. This is a big deal that has yet to hit >the fan so to sp

Re: Window sprinklers

2013-02-21 Thread MPhelps
: Friday, February 22, 2013 01:15 AM To: sprinklerforum@firesprinkler.org Subject: Re: Window sprinklers >From what I understand Tyco was not invited to the hearings for the proposed >changes and the rug was pulled out from under them in regard to the Tyco WS >sprinkler for 1hr and 2hr eq

Re: Window sprinklers

2013-02-21 Thread AKS-Gmail-IMAP
x: 952.229.2923 >>> ccah...@burnsmcd.com >>> www.burnsmcd.com >>> >>> Proud to be one of FORTUNE's 100 Best Companies to Work For >>> *Registered in: MN >>> >>> >>> >>> >>> -Original Messag

RE: Window sprinklers

2013-02-21 Thread Russell & Carol Gregory
I presume you mean a window with two panes separated by a vertical mullion. By most Codes/Rules: If the sprinkler/drencher is located centred on the mullion then one is OK. If mullion is less then 40mm proud of surface it can be ignored. Otherwise each pane of a window must be sprayed individually.

Re: Window sprinklers

2013-02-21 Thread bcasterline
ebruary 21, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona : Pretty sure you d

Re: Window sprinklers

2013-02-21 Thread Justin Reid
rg > [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of > bcasterl...@fsc-inc.com > Sent: Thursday, February 21, 2013 2:26 PM > To: sprinklerforum@firesprinkler.org > Subject: RE: Window sprinklers > > I think only horizontal mullions are considered an obstruction

RE: Window sprinklers

2013-02-21 Thread Cahill, Christopher
ginal Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of bcasterl...@fsc-inc.com Sent: Thursday, February 21, 2013 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers I think only horizontal mul

RE: Window sprinklers

2013-02-21 Thread bcasterline
I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona : Pretty sure you do. The mullion acts as a barrier. More than likely if you present the dilemma to the

RE: Window sprinklers

2013-02-21 Thread Rod DiBona
Pretty sure you do. The mullion acts as a barrier. More than likely if you present the dilemma to the A/E team they change the window. Rod at Rapid -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva

RE: WINDOW SPRINKLERS

2010-04-03 Thread Thom McMahon
riday, April 02, 2010 7:02 PM To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS Reliable Model FM for one. They are not listed to make the glass 1 hour rated, but they are listed for exposure protection. Greg McGahan Living Water Fire Protection (850) 937.1850 | Fax (850) 937.1

RE: WINDOW SPRINKLERS

2010-04-02 Thread Greg McGahan
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Friday, April 02, 2010 10:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs

Re: WINDOW SPRINKLERS

2010-04-02 Thread George Medina Jr
2.8K heads. George Medina Jr. -Original Message- From: Greg McGahan To: sprinklerforum@firesprinkler.org Sent: Thu, Apr 1, 2010 7:01 pm Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. I take the word "sill" iterally when apply

RE: WINDOW SPRINKLERS

2010-04-02 Thread John Drucker
forum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS The NRC Canada's IRC has an interesting article on the use of SSP QR heads to protect tempered glass windows, but I don't believe ICC has adopted any of these yet. http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html Thom McMahon, SE

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
The NRC Canada's IRC has an interesting article on the use of SSP QR heads to protect tempered glass windows, but I don't believe ICC has adopted any of these yet. http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Ste

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. Greg Mc

RE: WINDOW SPRINKLERS

2010-04-01 Thread Greg McGahan
On Behalf Of Steve Leyton Sent: Thursday, April 01, 2010 2:53 PM To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS So long as the water can sheet down the glass from point of contact at the top, to the bottom of each panel, you can do it. As Thom said, refer to the data sheet for

RE: WINDOW SPRINKLERS

2010-04-01 Thread Steve Leyton
10 12:52 PM To: sprinklerforum@firesprinkler.org Subject: RE: WINDOW SPRINKLERS George, The objective is that the entire surface of the glass be wetted. John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ -Or

RE: WINDOW SPRINKLERS

2010-04-01 Thread John Drucker
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 3:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½" mullions are vertical and was asking if each panel required sep

RE: WINDOW SPRINKLERS

2010-04-01 Thread Thom McMahon
Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 1:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½" mullions are vertical and was asking if each panel required separate sprinklers for them exceeding 1". Than

RE: WINDOW SPRINKLERS

2010-04-01 Thread Robert Thompson
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Thursday, April 01, 2010 2:31 PM To: sprinklerforum@firesprinkler.org Subject: Re: WINDOW SPRINKLERS I apologize for not being more clear, the 2½" mullions are vertical and was asking if each

Re: WINDOW SPRINKLERS

2010-04-01 Thread George Medina Jr
2010 12:22 pm Subject: RE: WINDOW SPRINKLERS You're not allowed horizontal mullions or molding. The glazing can be eparated by vertical mullions so long as each panel has its own sprinkler, but orizontal bumps are a deal-breaker. Steve Leyton rotection Design & Consulting an Diego

RE: WINDOW SPRINKLERS

2010-04-01 Thread Steve Leyton
You're not allowed horizontal mullions or molding. The glazing can be separated by vertical mullions so long as each panel has its own sprinkler, but horizontal bumps are a deal-breaker. Steve Leyton Protection Design & Consulting San Diego, CA -Original Message- From: sprinklerfor

RE: Window sprinklers

2010-03-09 Thread John Drucker
S-Gmail-IMAP Sent: Monday, March 08, 2010 11:47 PM To: sprinklerforum@firesprinkler.org Subject: Re: Window sprinklers In regard to the first question about to WS or not to WS, note that the building code is: On Mar 8, 2010, at 9:59 PM, John Drucker wrote: > BETWEEN 4 INCHES AND 12 INCHES (10

Re: Window sprinklers

2010-03-08 Thread AKS-Gmail-IMAP
In regard to the first question about to WS or not to WS, note that the building code is: On Mar 8, 2010, at 9:59 PM, John Drucker wrote: > BETWEEN 4 INCHES AND 12 INCHES (102 MM AND 305 MM) AWAY > FROM THE GLASS AND DESIGNED SO THAT THE ENTIRE SURFACE OF THE GLASS > IS WET > UPON ACTIVATION

RE: Window sprinklers

2010-03-08 Thread John Drucker
ch 08, 2010 4:42 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: I agree, Bob. My dear friend John Drucker would be disappointed in me for forgetting about the ability of the building code in providing such prescriptive alternatives. My intent was to just make the distincti

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
ss Sent: Monday, March 08, 2010 4:11 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Wait. You mean this exterior dry horizontal sidewall head I'm supposed to center over the exterior window connected to the wet system piping in the ceiling might not work the way the en

RE: Window sprinklers

2010-03-08 Thread Tom Duross
Wait. You mean this exterior dry horizontal sidewall head I'm supposed to center over the exterior window connected to the wet system piping in the ceiling might not work the way the engineer drew it? Buy an engineer drew it? It's on the drawring? (my apologies, a sore spot still..) Wong Not un

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
Behalf Of Sal Izzo (TECH- 103) Sent: Monday, March 08, 2010 1:42 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: I agree, Bob. My dear friend John Drucker would be disappointed in me for forgetting about the ability of the building code in providing such prescriptive

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: Wasn't the whole Atrium glass issue because the walls around an atrium were being treated like exposure protection, not as rated assembly compliance? What I think I heard, and could be wrong, was that SSP/ssu closely spaces we

RE: Window sprinklers

2010-03-08 Thread Sal Izzo (TECH- 103)
From: sprinklerforum-boun...@firesprinkler.org [sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo [bcap...@cox.net] Sent: Monday, March 08, 2010 4:11 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Sal, I am not challenging your knowledge or

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
ssage- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Monday, March 08, 2010 1:21 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Bob: Wasn't the whole Atrium glass issue because the walls around

RE: Window sprinklers

2010-03-08 Thread Thom McMahon
- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob Caputo Sent: Monday, March 08, 2010 2:12 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers Sal, I am not challenging your knowledge or expertise, and while I

RE: Window sprinklers

2010-03-08 Thread Thom McMahon
1:06 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers In answering this question, one must first ask if there is fire resistance rating required to be maintained with this installation. Only listed window sprinklers are tested and listed to provide an actual fire resistance

RE: Window sprinklers

2010-03-08 Thread Bob Caputo
Cantara Lane, Vista, CA 92081 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sal Izzo (TECH- 103) Sent: Monday, March 08, 2010 12:06 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window sprinklers In ans

RE: Window sprinklers

2010-03-08 Thread Sal Izzo (TECH- 103)
In answering this question, one must first ask if there is fire resistance rating required to be maintained with this installation. Only listed window sprinklers are tested and listed to provide an actual fire resistance rating for glazing. This is because these sprinklers are tested in accord

RE: Window sprinklers

2010-03-08 Thread Chris Cahill
Only the person that specified the rated wall or alternate means and methods for the glass can answer that. You'll note NFPA 13 doesn't have anything for a contractor to follow, thus this is architect or engineering work to decide how to do it. FWIW I've seen both and am comfortable with SS when

Re: Window Sprinklers

2009-03-21 Thread rahe . loftin
Everything you need to know is in the ICC Legacy report including why you need a pony wall. Rahe Loftin - Original Message - From: "Cliff Whitfield" [cl...@fire-design.com] Sent: 03/21/2009 05:04 PM EST To: Subject: RE: Window Sprinklers Thom, Great info. Than

RE: Window Sprinklers

2009-03-21 Thread Cliff Whitfield
Thom, Great info. Thanks. Cliff -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Saturday, March 21, 2009 4:00 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers There

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
ICC link to report http://www.icc-es.org/reports/pdf_files/NES/NER516.pdf Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- ___ Sprink

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Thom, That brings up another issue I've been wondering about. I am being required to use these on both sides of the windows. I have not studied the details yet but if the top of the window is at 7' AFF and the ceiling is at

RE: Window Sprinklers

2009-03-21 Thread Cliff Whitfield
boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Saturday, March 21, 2009 12:34 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Also unless the windows extend to the ceiling the widow sprinklers will be placed lower th

RE: Window Sprinklers

2009-03-21 Thread Thom McMahon
Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff Whitfield Sent: Saturday, March 21, 2009 7:20 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers

RE: Window Sprinklers

2009-03-21 Thread Cliff Whitfield
sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron Sent: Saturday, March 21, 2009 8:13 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers I would say no you can't use them for floor coverage. On the plus side

RE: Window Sprinklers

2009-03-21 Thread Fletcher, Ron
I would say no you can't use them for floor coverage. On the plus side though I don't think you have to worry about cold soldering from the ceiling sprinklers either. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ 85024 -Original Message- From: sprinklerforum-boun...@firesprinkler.or

RE: Window Sprinklers

2008-10-06 Thread Fletcher, Ron
Subject: RE: Window Sprinklers Its important to keep the context of the building code clear. First 2006 IBC Section 704 applies to EXTERIOR WALLS. 2006 IBC 704.12 "Opening Protection" applies to; "WINDOWS in EXTERIOR WALLS REQUIRED to have protected openings in accordance with ot

RE: Window Sprinklers

2008-10-03 Thread John Drucker
D] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Friday, October 03, 2008 2:52 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers You DO NOT need building code permission use these heads in an unsprinklered building. They comply with the building code. The building

RE: Window Sprinklers

2008-10-03 Thread Chris Cahill
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Friday, October 03, 2008 11:16 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Yes but the building code does not! So I guess where you have no building code your OK. Thom McMahon, SET Firetech,

RE: Window Sprinklers

2008-10-03 Thread Fletcher, Ron
ay to all, Ron Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Justin Reid Sent: Friday, October 03, 2008 10:17 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers In an exposure fire like the one described, it would be the respons

RE: Window Sprinklers

2008-10-03 Thread Justin Reid
In an exposure fire like the one described, it would be the responsibility of the design team to make sure that the fusible link of the sprinkler head is in an area that can "sense" the exposure threat. NFPA 80A discusses this concept in its appendix. So the glass bulb in the sprinkler head shou

RE: Window Sprinklers

2008-10-03 Thread Steve Leyton
That explains a lot about the composition of fire-rated glazing. I don't know what the treatment is that's applied to "Fire-Lite" or other rated glass but the knock on those products is that they are exorbitantly expensive. It's not as if you can order up pieces of it - you have to purchase

RE: Window Sprinklers

2008-10-03 Thread Thom McMahon
Yes but the building code does not! So I guess where you have no building code your OK. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTE

RE: Window Sprinklers

2008-10-03 Thread Thom McMahon
This thread has already gone on way too long but I can't let this slide. Scott: If your installing window sprinklers in an unsprinklered building, your already outside the scope of the listing and the building code, so your using your "Engineer" Status to say that this will work! And with that your

RE: Window Sprinklers

2008-10-03 Thread Fletcher, Ron
Thanks man, great information. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... Sent: Friday, October 03, 2008 5:03 AM To: sprinklerforum@firesprinkler.org Subject: Window Sprinklers Pagni, at Be

RE: Window Sprinklers

2008-10-02 Thread Russell
PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Thursday, October 02, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers ToMAYto, toMAHto - my point only being that it's not as if these sprinklers just showed up with the I-codes. Quell is ne

RE: Window Sprinklers

2008-10-02 Thread Steve Leyton
l relative. Steve Leyton Protection Design & Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Thursday, October 02, 2008 5:12 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 10 years is new wh

RE: Window Sprinklers

2008-10-02 Thread Fletcher, Ron
: Thursday, October 02, 2008 5:12 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 10 years is new when you've been in this trade for 30 yrs. wouldn't you think? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8

RE: Window Sprinklers

2008-10-02 Thread Russell
10 years is new when you've been in this trade for 30 yrs. wouldn't you think? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] ___ Sprinklerforum mailing list http://lists.fires

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
MAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 10:08 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The obvious answer would be heat that directly threatens the glass; a sprinkler could react directly to heat on the same side or to heat radiated

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
Wednesday, October 01, 2008 12:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Rated glass walls have been used for ages but the Tyco window sprinkler is fairly new so I've been wondering what has been done in the past to address this issue architecturally wise. I ca

RE: Window Sprinklers

2008-10-01 Thread Chris Cahill
icc-es.org/reports/pdf_files/NES/NER516.pdf John Drucker -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 10:28 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The window sprinkler was

RE: Window Sprinklers

2008-10-01 Thread Russell
Rated glass walls have been used for ages but the Tyco window sprinkler is fairly new so I've been wondering what has been done in the past to address this issue architecturally wise. I called an architect and questioned him on it. He said that a long time ago one could use wire glass. Now he uses

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
tober 01, 2008 10:24 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers If that happens what's the problem? If FD is on the scene and attacking the fire then most likely occupants are out, hose streams are in play and sprinklers at the glass are a non-issue. What about

RE: Window Sprinklers

2008-10-01 Thread John Drucker
ROTECTED] On Behalf Of John Drucker Sent: Wednesday, October 01, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers 2006 IBC 704.12 provides for exterior window opening utilizing a water curtain. "Exception - Opening protectives are not required where th

RE: Window Sprinklers

2008-10-01 Thread Craig.Prahl
esday, October 01, 2008 1:08 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers That was my point exactly. Not how to install the head per the listing. A manual system would be more dependable than a closed head system with no heat collection. Here's a what if. What if ther

RE: Window Sprinklers

2008-10-01 Thread Justin Reid
] -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a note about the mentioning of "sprinkler activation". The

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
the window sprinkler has activated. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers J

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
. Steve Leyton Protection Design & Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Wednesday, October 01, 2008 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a note about the menti

RE: Window Sprinklers

2008-10-01 Thread R Richardson
I believe the issue is similar to in-rack sprinklers in that the activation is more or less direct flame impingement. If there is enough heat to jeopardize the side of a building the head will likely activate. Rich Richardson Seattle Fire Department >>> "Russell" <[EMAIL PROTECTED]> 10/01/2008

RE: Window Sprinklers

2008-10-01 Thread Thom McMahon
79-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 9:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers So the test assumes the glass remains intact until s

RE: Window Sprinklers

2008-10-01 Thread Russell
Just a note about the mentioning of "sprinkler activation". The data sheet states that the advantages are its ability to wet the entire glass and the quick activation time. Well, that quick activation time is a mystery to me because the data states that there is no specific distance below the ceili

RE: Window Sprinklers

2008-10-01 Thread John Drucker
icial (AHJ) Red Bank, NJ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 10:28 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The window sprinkler was tested using the exact same criteri

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Wednesday, October 01, 2008 8:29 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Yes. Steve Leyton Protection Design & Consulting San Diego, CA -Original Message- From: [EMAIL PROTE

RE: Window Sprinklers

2008-10-01 Thread Craig.Prahl
[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers And nobody thinks that might be a problem? I have installed these heads four feet below a ceiling and outside with only the mullion to act as a heat

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
01, 2008 8:19 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Same as for any rated wall or partition. It can't do it's job if it's not intact. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO B

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
Yes. Steve Leyton Protection Design & Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 8:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers So the

RE: Window Sprinklers

2008-10-01 Thread Craig.Prahl
EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, October 01, 2008 11:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers So the test assumes the glass remains intact

RE: Window Sprinklers

2008-10-01 Thread Fletcher, Ron
@firesprinkler.org Subject: RE: Window Sprinklers The window sprinkler was tested using the exact same criteria as is used to establish any other rated assembly. A test fire is built on one side of the subject and burned for the duration of the rating and then there's a steady-stream hose test

RE: Window Sprinklers

2008-10-01 Thread Steve Leyton
yton Protection Design & Consulting San Diego, CA -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, October 01, 2008 6:43 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Just a guess but I thin

RE: Window Sprinklers

2008-10-01 Thread bill . brooks
, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell Original Message Subject: RE: Window Sprinklers From: "Bill Minkel" <[EMAIL PROTECTED]> Date: Wed, October 01, 2008 9:27

RE: Window Sprinklers

2008-10-01 Thread Bill Minkel
Ah, Gotcha Bill Minkel, Designer Dallas, TX -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Tuesday, September 30, 2008 3:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Of course it's MORE than ade

RE: Window Sprinklers

2008-09-30 Thread Thom McMahon
Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Tuesday, September 30, 2008 11:29 AM To: sprinklerforum@firesprinkler.org Subject: RE: Wind

RE: Window Sprinklers

2008-09-30 Thread Craig.Prahl
D] On Behalf Of Roland Huggins Sent: Tuesday, September 30, 2008 2:24 PM To: sprinklerforum@firesprinkler.org Subject: Re: Window Sprinklers IT has been reported to me (equates to I have not checked the cut sheet) that the WS sprinklers can not be used on load bearing walls. Has anyone encountered this a

Re: Window Sprinklers

2008-09-30 Thread Roland Huggins
IT has been reported to me (equates to I have not checked the cut sheet) that the WS sprinklers can not be used on load bearing walls. Has anyone encountered this aspect? Roland On Sep 30, 2008, at 8:37 AM, Steve Leyton wrote: The Tyco tests very conspicuously did not, nor does the listing

Re: Window Sprinklers

2008-09-30 Thread Justin Reid
TED] On Behalf Of Steve Leyton Sent: Tuesday, September 30, 2008 7:54 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers A HA!!! That's the point, isn't it? That the architect failed to completely design the building and account for the protection of windows a

RE: Window Sprinklers

2008-09-30 Thread Bill Minkel
, September 30, 2008 11:07 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Now the "Window sprinkler" is an alternate to 2Hr. rating, but in the situation described, it would appear the school is a fully sprinklered structure, so under the building code they may ha

RE: Window Sprinklers

2008-09-30 Thread Mark Cummings
nsive swimming pools. :-( Regards, Mark Cummings Sydney, Australia [EMAIL PROTECTED] -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Wednesday, 1 October 2008 12:39 AM To: sprinklerforum@firesprinkler.org Subject: RE:

RE: Window Sprinklers

2008-09-30 Thread Thom McMahon
9:55 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers Well all that's being said gives me cause to drop this hot potato in the hands of the architect AND engineer and be sure I have a written directive on how to proceed. I was thinking that I could fall back on the old d

RE: Window Sprinklers

2008-09-30 Thread Thom McMahon
ilto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Tuesday, September 30, 2008 9:38 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprinklers The Tyco tests very conspicuously did not, nor does the listing include doors or moving casement windows. Fixed glass only, no horizont

RE: Window Sprinklers

2008-09-30 Thread Russell
Well all that's being said gives me cause to drop this hot potato in the hands of the architect AND engineer and be sure I have a written directive on how to proceed. I was thinking that I could fall back on the old days and do what was done thousands of times in the past, but I guess not. Thanks

RE: Window Sprinklers

2008-09-30 Thread Steve Leyton
ndow Sprinklers Can glass door be protected by a window sprinkler? Ron Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Tuesday, September 30, 2008 8:00 AM To: sprinklerforum@firesprinkler.org Subject: RE: Window Sprink