Ron Greenman wrote:
Once I was called incompetent by the architect because in the field
there was one inch of clear space between the bottom of the beams
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Terri Leyton wrote:
I've been trying to send a post with attachments and it would appear to
be too big for our servers. So, let's try this.
Below is a letter from
professional, there will be no charge for this
assistance.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Todd Williams - FPDC wrote:
Personally, I don't think
that those letters by themselves don't convey
competence. What a pity.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Steve Leyton wrote:
I wonder how many
a substantial fire and oil resistant sealant to make sure
that hot oil can't flow from one bay to the
other.
Stewart
Original Message:
-
From: Dee Lockwood [EMAIL PROTECTED]
Date: Thu, 6 Nov 2008 07:43:57 -0800
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire resistant barriers
fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
danarbel wrote:
Question regarding the number of ESFR heads required for hydraulic calc.
The nominal number is 12.
There was a requirement to add 2 heads
at the opposite level.
Maybe I just don't see it. Wouldn't be the first time, and probably not
the last.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Thom McMahon wrote:
A Penny wise and Pound foolish Attitude. You Can NOT afford to miss the
training, and learning experiences offered! We
) 425-1001
[EMAIL PROTECTED]
---
Sent from a handheld, please excuse any misspelled words.
-Original Message-
From: [EMAIL PROTECTED] [EMAIL PROTECTED]
To: AFSA Forum SprinklerFORUM@firesprinkler.org
Sent: 9/27/08 10:04 AM
Subject: Re: which pipe
sprinklers hided above
the dome is a legal and possible design!?
Thank you experts,
George Lau
--- On Wed, 9/10/08, Allan Seidel [EMAIL PROTECTED] wrote:
From: Allan Seidel [EMAIL PROTECTED]
Subject: Re: Help!! Sprinkler in Planetrium
To: sprinklerforum@firesprinkler.org
Date: Wednesday
on the phone
I'll be glad to talk over some of the other issues.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
[EMAIL PROTECTED] wrote:
An AHJ wants
in Table 8.7.2.2.1 shall be
permitted under the overhead
doors.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
IPA wrote:
Quick question:
When you
, and the maximum spacing is 15'.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Russell wrote:
Okay here's one. Please someone direct me to the text that states
PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe
installed.
There are none listed for recessed sprinklers.
Doesn't phase them a bit. When I asked how it was to be resolved, the
answer was That's your problem, not mine.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
Charles,
Is there any reason you can't tap off the domestic service?
Or do they require a minimum 2-1/2 for that too?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http
Joe,
If you can rip that video, please get it to me and I'll put it in a
place where anyone who wants to can
download it and see the results of your testing.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Eckard, Mark - Mark E wrote:
I was referring to the 2002 Edition of NFPA which is still adopted by a
majority of the US.
Mark E. Eckard S.E.T.
Engineering Manager
Lowe's
PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Eckard, Mark - Mark E wrote:
Another issue with seismic bracing design and calculation is the fact
that NFPA 13 only applies to seismic design category A, B, C.
Categories A and B usually
?*
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Dennis J Briggs Jr. wrote:
Im having trouble finding the information that relates to setting the pressure
.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Original Message
Subject: unified facilities criteria question
From: Tambini, Ed [EMAIL
PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
IMPORTANT NOTICE: This correspondence is not a Formal
Interpretation issued pursuant to NFPA Regulations. Any opinion
expressed is the personal opinion of the author and does not necessarily
with what your understanding of the process would be?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
IMPORTANT NOTICE: This correspondence is not a Formal
pocket 13-17 sprinklers in
a 224 sf room.
Just my thoughts.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Bob Knight wrote:
I'm working on a home (13D
moved
all the storage stuff around.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Roland Huggins wrote:
Good catch. Memory says we intended to incorporate
.
Interesting to be sure.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
[EMAIL PROTECTED] wrote:
I have a tank farm with deluge sprinkler protection on the vessels
Dave,
If G. Tim can't help you or you can't get in touch with him give me a
call offline and I'll see if I can.
Best regards,
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http
Joe,
I hate to disagree with you but wouldn't they be incinerated first,
based on Boyle's law?
Just wondering.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com
that
locating the sprinkler so that it might discharge
from the adjacent wall would be a reasonable approach, however I think
you hit it on the head when you
mentioned that the furniture is movable.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto
when applying this modifier. The lower SG types are
Northern White Cedar (0.32),
Western Red Cedar (0.34).
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
to admit that the book I have on this is over 40 years
old, and there may be very different
species of wood being used out there now. More questions for the
structural engineer of record, I guess.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto
fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Jimmy Waite wrote:
Tyco's attic sprinklers are out b/c we only have a 3 in 12 pitch, all of
their heads start at 4 in 12.
Jimmy
-Original Message-
From: [EMAIL
Standards Commission by the city, county, or city and county where it
will apply,
along with the adopting ordinance and any findings of the city, county,
or city and
county
Hope that helps.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL
and diameter, the loss is approximately 0.65 psi.
Have I read that wrong?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
[EMAIL PROTECTED] wrote:
As an aside, when
that they
live to do stuff like this.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
IMPORTANT NOTICE: This correspondence is not a Formal
Interpretation issued
vulgar
enough to express myself clearly at his perspective.
Just thought I'd vent here.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
braced eliminates their
load from the mains.
--
PARSLEY CONSULTING
Ken Wagoner
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.parsleyconsulting.com http://www.parsleyconsulting.com/ website
IMPORTANT NOTICE: This correspondence is not a Formal
buildings of
three stories or more to have a class I standpipe in all stairs which
connect two or more stories.
Otherwise, what everyone else said.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http
CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
art wrote:
What good is pressure 5' below grade. Don't you expect pressures to be at
grade or at finished floor? Adjust
.
Any help, greatly appreciated.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
___
Sprinklerforum mailing list
).
Is that about right?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Ed Kramer wrote:
Ken,
Question #1: Yes
Question #2: it depends. For light hazards
and
to Benjamin Franklin. I'd do some research on it, but I don't have
tiiime. (c.f. Joe Cage).
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Steve Leyton wrote
with them first.
As for the load capacity I would go with what the manufacturer's data
sheet allows.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Bob Knight
to calculate only five flowing heads, and if the design included
only standard spray sprinklers it must include seven flowing sprinklers.
At least that would be my read on it.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Joe Burtell wrote:
I have not worked with FM much and I am hoping someone can verify my design
is correct.
4,000 S.F. warehouse for carpet storage to max. 5
, A.7.1, where it's noted that the
building height will determine the number of vertical zones.
Unless Mayor Leyton's dad tells me this is in error, that's my
perspective.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
that a 65 year old structural design book has all that
relevant information.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
å... wrote:
2007 NFPA 13
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Jones, Nancy wrote:
Is it the intent of 6.7.3 and the commentary for 6.8 in the 2002 edition of
13R to require a detached garage to be protected?
Thanks
CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Richard Battershell wrote:
Help. I have a fire official requiring us to do a four head bucket test on
a NFPA 13r system
seem to me that you can run the drain line in CPVC exposed
without deviating from NFPA requirements. Now whether the manufacturer
will stand behind it is another consideration.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e
a crime wave.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
Travis Mack wrote:
Well, we better get the local police involved. I can't tell you how many
times
.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com http://www.ParsleyConsulting.com website
___
Sprinklerforum mailing list
Sprinklerforum
Rahe,
That's why NFPA-13 has the following section 9.1.1.6.6, so that rods
used to support trapeze members are sized to support the pipe itself,
not the pipe used for the trapeze.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] mailto:[EMAIL