[Sprinklerforum] Re: Baled Pulp Fibers

2023-03-11 Thread Art Tiroly
Would this be similar to baled corrugated box board?

These are very dense bundles that can only allow a surface burning.

Yes it's class 3.

Is this stacked on the floor in large piles or in racks?

NFPA 13 should have the answer.

 

Art

 

From: James Crawford  
Sent: Friday, March 10, 2023 4:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Baled Pulp Fibers

 

Looking for a little help from those smarter than me

 

We have a client that wants to store baled pulp fiber to a height of 20' but
all I can find is NFPA #13 that allows 15' and FM that allows 16'.

 

Is there anything out there that gives a protection scheme for higher
storage?

 

Thank You

 

James Crawford

Phaser Fire Protection Ltd.

Phone 604-888-0318

Cel: 604-790-0938

Email jcrawf...@phaserfire.ca <mailto:jcrawf...@phaserfire.ca> 

Web: www.phaserfire.ca <http://www.phaserfire.ca> 

 


_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: [EXTERNAL] Re: Fire Station Apparatus Bay

2023-02-17 Thread Art Tiroly
Some of the new 5” hose in the bed of the truck is plastic covered flexible 
material.

 

Art Tiroly

 

From: Brett Peters  
Sent: Thursday, February 16, 2023 4:47 PM
To: Discussion list on issues relating to automatic fire sprinklers 

Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Fire Station Apparatus Bay

 

possibly but OHII covers 10'-0 of class IV commodity, personally I don't see 
how the fire trucks or equipment in the apparatus bay would take you past that.


 

 

Thanks

 

Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

br...@proudline.ca <mailto:br...@proudline.ca> 

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca <http://www.proudline.ca/> 

 

Proudline now offers ULc listed monitoring services, please contact 
m...@proudline.ca <mailto:m...@proudline.ca>  for more information

 

 

 

   

 

 

On Thu, Feb 16, 2023 at 2:43 PM Prahl, Craig mailto:craig.pr...@jacobs.com> > wrote:

I don’t know that I’d call it a “big” difference and for clarification I’m not 
comparing this to an ignitable liquid warehouse.  But when you look at the 
level of potential fuel loading (not just diesel) and the value of the contents 
of an apparatus bay which can easily reach into multiple millions of dollars 
not including the structure and loss of use in a fire event, I’d love to see 
the rationale behind the development of criteria for buildings like this.  It’s 
just a point of curiosity.  

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
 www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606 

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: Brett Peters mailto:br...@proudline.ca> > 
Sent: Thursday, February 16, 2023 4:33 PM
To: Discussion list on issues relating to automatic fire sprinklers 
mailto:sprinklerforum@lists.firesprinkler.org> >
Subject: [EXTERNAL] [Sprinklerforum] Re: Fire Station Apparatus Bay

 

Craig

I believe there is a big difference between storage requirements for diesel 
fuel and fuel in a vehicles fuel tank, if the space was used for the storage of 
diesel fuel than OH2 might not be adequate but this is not a fuel storage 
warehouse and the amounts of fuel found in the trucks probably falls within the 
building code allowances for an unprotected building and certainly with the 
tables for a building protected with a sprinkler system.


 

 

Thanks

 

Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

br...@proudline.ca <mailto:br...@proudline.ca> 

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca 
<https://urldefense.com/v3/__http:/www.proudline.ca/__;!!B5cixuoO7ltTeg!AlZ8AmeMUVxYNoVJPQ7ArPXFalsEVZOJnOdXtSBo72cKeXRdWM_dWE96_m1EBSFYImnCzLFdhDs_yE9t66M$>
 

 

Proudline now offers ULc listed monitoring services, please contact 
m...@proudline.ca <mailto:m...@proudline.ca>  for more information

 

 

 

   

 

 

On Thu, Feb 16, 2023 at 2:23 PM Prahl, Craig mailto:craig.pr...@jacobs.com> > wrote:

It’s funny, if the diesel fuel was in anything other than a truck, it would be 
EH2.  Some of the criteria makes very little sense, especially in cases like 
this where a fuel spill would most likely end up being shielded from overhead 
sprinklers and is a non-miscible hydrocarbon.  

 

Wait until we have a fire involving an electric fire apparatus.  

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |  
<mailto:craig.pr...@jacobs.com> craig.pr...@jacobs.com |  
<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
 www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606 

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: Brian Harris mailto:bhar...@bvssystemsinc.com> > 
Sent: Thursday, February 16, 2023 2:42 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [EXTERNAL] [Sprinklerforum] Fire Station Apparatus Bay

 

I’ve seen Apparatus Bays in fire stations protected both as OH1 & OH2. Seems 
per code OH1 (car parking) would be appropriate?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com 
<https://urldefense.com/v3/__http:/bvssystemsinc.com/__;!!B5cixuoO7ltTeg!AFrgnB0i9ZV8hwI9dybPcbue3rE1t2eKusy43_5MkD4PAHEE4yJ9GqO7i0TMVkm-8UzBMjzH3ujNQiAL7ew7Dp6x$>
 

Phone: 704.896.9989

Fax: 704.896.1935

 

 

 


  _  



NOTICE - This communication may contain

[Sprinklerforum] Re: NFPA 21 VERSUS 22

2022-12-03 Thread Art Tiroly
Using an ESFR sprinkler at 100 GPM for 12 sprinklers may be more of a cost 
savings.

 

Art

 

From: Trillium Fire Sprinkler Design INC  
Sent: Saturday, December 03, 2022 7:53 AM
To: 'Discussion list on issues relating to automatic fire sprinklers' 

Subject: [Sprinklerforum] Re: NFPA 21 VERSUS 22

 

Thanks Ken. Exactly what I was thinking. Just needed clarification.

Troy

 

From: Ken Wagoner mailto:k...@parsleyconsulting.com> > 
Sent: December 2, 2022 11:57 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [Sprinklerforum] Re: NFPA 21 VERSUS 22

 

It would be helpful in we were shown where you came up with the references for 
both a density of .325 and an increase of 175%, and perhaps most of all where 
you're directed to "22" (guessing you meant Chapter 22?), as that chapter 
covers the use of CMSA sprinklers.

Table 21.4.1.2.2.1 addresses class II, non-encapsulated storage to 25' height, 
with 8' aisles to figure 21.4.1.2.2.1(b), and curves A or B.  Curve a for high 
temp sprinklers shows 0.325 gpm/ft² over 2,000 ft², which matches what you've 
quoted. If ordinary temp sprinklers are selected (curve B) the density jumps to 
0.375 gpm/ft².

And yes, the density is required to be increased per the graph in Figure 
21.4.1.7.1 to 175% of the values from the curves when the height of storage 
exceeds 20'.  That would result in densities of ± 0.569 for high temps and ± 
0.656 for ordinary temps.
 
I hope this is of some value,

Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181 
Visit the website 
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK=1>
  

On 12/2/2022 9:23 AM, Trillium Fire Sprinkler Design INC wrote:

I  have a warehouse that has double row rack storage to 25 feet with 8 foot 
aisles. Class II commodity non encapsulated.

 

21 says that .325 density apply the increase of 175%  for  the 25 foot storage. 
Using CMDA sprinklers

 

But then says if using CMDA sprinklers use 22.

 

I am confused!

 

Which chapter do I use.

 

 

 

 

 
_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org 
<mailto:sprinklerforum-le...@lists.firesprinkler.org> 

 


_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Fire pump package weight ?

2022-09-14 Thread Art Tiroly
Ask a firte pump sales agent, they will know.

-Original Message-
From: Sean Lockyer  
Sent: Thursday, September 15, 2022 12:25 AM
To: Discussion list on issues relating to automatic fire sprinklers

Subject: [Sprinklerforum] Re: Fire pump package weight ?

1500 gpm, 100 hp

-Original Message-
From: Art Tiroly  
Sent: Thursday, September 15, 2022 12:22 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'

Subject: [Sprinklerforum] Re: Fire pump package weight ?

What GPM and what HP?

-Original Message-
From: Sean Lockyer 
Sent: Thursday, September 15, 2022 12:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Fire pump package weight ?

About how much would you surmise the weight of an electric horizontal
split-case fire pump package (include enclosure) would weigh ? 

    Sean Lockyer
    Project Designer   
  















_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org


[Sprinklerforum] Re: Fire pump package weight ?

2022-09-14 Thread Art Tiroly
What GPM and what HP?

-Original Message-
From: Sean Lockyer  
Sent: Thursday, September 15, 2022 12:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Fire pump package weight ?

About how much would you surmise the weight of an electric horizontal
split-case fire pump package (include enclosure) would weigh ? 

    Sean Lockyer
    Project Designer   
  















_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org


RE: filling a pre-action system with water

2022-02-17 Thread Art Tiroly via Sprinklerforum
The high pressure water in=rush compresses the air in the system.
The velocity slows as the air pressure is compressed. I don't believe there
is water hammer potential because the air creates a cushion.

Art Tiroly
ATCO/Tiroly Fire Protection

-Original Message-
From: Sprinklerforum  On
Behalf Of Matt Grise via Sprinklerforum
Sent: Thursday, February 17, 2022 1:10 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise 
Subject: filling a pre-action system with water

I am curious about how single-interlock pre-action systems get filled up
with water:

When the detectors activate and open the deluge valve but no sprinkler head
is open - how quickly does the piping actually fill up with water? Is it
fast enough that you need to worry about a water hammer if the piping fills
before the heads start to open?

I did not know if the supervisory air just kind of oozes out and lets the
water in slowly, or if the valve opens, (maybe kicks the pump on) and really
blasts it in there.

Does anyone out there have experience with this sort of thing? I would
definitely appreciate some insight into how it actually goes down.

Thanks!

Matt

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: question about Storage height

2022-01-26 Thread Art Tiroly via Sprinklerforum
Is the spill container open top? That will be an issue. These sound like
plastic totes. If the liquid is not combustible the empty tote is still a
lot of plastic

Art

-Original Message-
From: Sprinklerforum  On
Behalf Of Scott Futrell via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:32 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell ; Mike Hairfield 
Subject: RE: question about Storage height

You didn't mention what the liquid is. If it is a hazardous material as
recognized by the International Fire Code then the 'empty' container is
still considered full unless completely cleaned.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum  On
Behalf Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, January 26, 2022 8:08 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Hairfield 
Subject: Re: question about Storage height

It should be 10 feet even though the other container is empty it's still
plastic.

Mike

From: Sprinklerforum  on
behalf of Steve Mackinnon via Sprinklerforum

Sent: Wednesday, January 26, 2022 9:02 AM
To: sprinklerforum@lists.firesprinkler.org

Cc: Steve Mackinnon ; Peter Howard

Subject: question about Storage height

Good morning all,

We have a storage situation where the liquid commodity is in a 5 foot
plastic storage cube, with an equally sized empty plastic container below.

The empty container below is only there to act as a spill collection vessel.

The question our office has been banging around, what is the storage
height???

Would this be considered 5 feet of storage or 10 feet?

Would you take any exception to the plastic containers (like when we change
the commodity classification with wood to plastic pallets)?

Thank you in advance
Steven
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesp
rinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.orgdata=04%7C
01%7C%7C0d961840310a423de85308d9e0d49405%7C84df9e7fe9f640afb435%
7C1%7C0%7C637788025897874973%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJ
QIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000sdata=gZPzEokK%2FC%2F
BPf%2FyCzVVjYGR3%2FRAFZEAkLsE2Cn2Qjk%3Dreserved=0
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Attic protection over a storage occupancy

2021-10-06 Thread Art Tiroly via Sprinklerforum
No building size is indicated. Does the building code require protection?  
Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of the
building and contents.

Art Tiroly

ATCO Fire Protection


-Original Message-
From: Sprinklerforum  On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give me
a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
storage in racks.  The building is a standard 4:12 wood truss building with
plywood sheathing at the bottom of the trusses (with a layer of fiberglass
batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
2x construction with fiberglass batts.  I can't come up with a reason I
can't protect the space below the plywood according to the storage
requirements (looking at .6/2600 dry system, rack storage of Gp A plastic to
20' max <5' clear, doing CMDA both because they barely have 18" clear and
they want a dry system) and the space above as an unused light hazard attic,
potentially with "back to back" style attic heads.  Anyone see a flaw with
this logic, or any other pitfalls to watch for due to this construction
scenario?  I don't love this scenario but the customer went out of their way
to avoid sprinklering the building origina  lly and built it to the bottom
dollar, but now a new insurance carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender.  You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR & Obstruction in Light Hazard

2021-02-01 Thread Art Tiroly via Sprinklerforum
I had a similar problem but worked it out with AHJ and he allowed the
obstructions with the ESFR's.

Art Tiroly

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford via Sprinklerforum
Sent: Monday, February 01, 2021 12:18 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: James Crawford
Subject: ESFR & Obstruction in Light Hazard

WE have a warehouse space that is protected with ESFR sprinkler heads, the
space is being used by an indoor tennis club.

The want to add some additional HVAC and some of the new ducting would
obstruct the ESFR sprinkler heads.

My question is do we still need to work to the same obstruction rules for
this application, fire load is minimal we would be delivering 1200gpm rather
then the 150gpm required, just seem like overkill.

Opinions please

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web: www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-- 
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 13 R in a single family home

2020-08-13 Thread Art Tiroly via Sprinklerforum
For a home worth multiple millions a 10 minute water supply for life safety may 
not be the best answer for property values.
There may be insurance savings to help pay for the extra cost for 13R.
Local requirements for high value homes may be the better value for the 
sprinkler system.

Art Tiroly

-Original Message-
From: Sprinklerforum  On Behalf 
Of Ken Wagoner via Sprinklerforum
Sent: Thursday, August 13, 2020 3:31 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ken Wagoner ; Matthew J Willis 
; Steve Leyton 
Subject: Re: 13 R in a single family home

Adding a few logs to this fire I have to share that the comment by Matt is very 
accurate.

I've dealt with many AHJ's here in California who when pushed over some issue 
on a single family home have responded with, "Just do a 13R system," without 
truly understanding the difference.  Here are a few notes which come to mind:

  * 13R requires an FDC, where 13D does not
  * 13R requires conformance with NFPA 25, and 13D does not
  * 13R requires a 30 minute water supply, 13D requires only 10 minutes
of water
  * 13R requires any pump provided to meet NFPA 20 conditions, as Matt
noted below.
  * 13R requires any pressure tank to be both listed, and conform to
NFPA 22, 13D only requires conformance to ASME standards, and makes
no reference to NFPA 22 in any portion of the text
  * 13R requires the total number of fixture units to be addressed in
the hydraulic calculations, if the supply serves both the fire
sprinkler and domestic water systems, 13D has no such requirement.
  * 13R requires a hydrostatic test conforming to NFPA 13 if more than
20 sprinklers are provided, and at 50 psi higher than the maximum
system pressure if less than 20 sprinklers are in the system, 13D
requires hydrostatic testing at system pressure if no FDC is provided.

I've almost run out of breath preaching to various AHJ's - if you wish to have 
calculations flowing up to four sprinklers, rather than the 2 sprinklers 
routinely called for in 13D, just say so.

sincerely,

*Ken Wagoner, SET
*Parsley Consulting*
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> *

**
On 8/13/2020 11:57 AM, Matthew J Willis via Sprinklerforum wrote:
> Common theme seems to be Townhomes.
>
> Just wanted throw this out..,
>
> Beware the subtle shift from 13D to 13R. It is more than just going from a 2 
> head calc to a possible 4 head calc and larger pipe.
>
> 13D is very careful to use the word "Pump" only. NFPA 20 is not referenced in 
> Chapter 2.
>
> 13R..., Not so much.
>
> Happy hunting!
>
> R/
> Matt
>
>
> Matthew J. Willis, CWBSP
> Design Manager /3-D Specialist
> Rapid Fire Protection Inc.
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>
>
>
>
>
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Steve Leyton via Sprinklerforum
> Sent: Thursday, August 13, 2020 11:53 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton 
> Subject: RE: 13 R in a single family home
>
> We're working on a project right now in San Diego with four 4-story townhomes 
> in a row and it's been code classified as R2; we're designing per NFPA 13 on 
> that one.
>
> Steve L.
>
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> Mark.Phelps via Sprinklerforum
> Sent: Thursday, August 13, 2020 10:29 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Mark.Phelps 
> Subject: RE: 13 R in a single family home
>
> San Francisco.
>
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Kyle.Montgomery via Sprinklerforum
> Sent: Thursday, August 13, 2020 8:06 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Kyle.Montgomery 
> Subject: [EXTERNAL] RE: 13 R in a single family home
>
> Out of curiosity, where are people building single family homes that 4+ 
> stories? I don't think I've ever seen one.
>
> -Kyle M
>
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Matthew J Willis via Sprinklerforum
> Sent: Thursday, August 13, 2020 7:27 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matthew J Willis 
> Subject: [EXTERNAL] RE: 13 R in a single family home
>
> Ahh. Excellent catch for us.
>
>
> Other requirements had me as well on mine.
>
> Thanks for the assist!
>
> R/
> Matt
>
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Steven Jenkins via Sprinklerforum
> Sent: Thursday, August 13, 2020 7:49 AM
> To: sprinklerforum@lists.firesprinkl

RE: Exemption for sprinklers

2020-06-02 Thread Art Tiroly via Sprinklerforum
What does the building code say regarding this construction and occupancy?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Larrimer, Peter A (HEFP\10NA5B) via Sprinklerforum
Sent: Tuesday, June 02, 2020 3:49 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\10NA5B)
Subject: Exemption for sprinklers

 

NFPA 101, 7.14 (2018) permits sprinklers to be omitted from "Normally
Unoccupied Building Service Equipment Support Areas".  These support areas
are not intended to be accessed by persons for maintenance. However, they
might have man-doors installed that would make them accessible and when they
are over 45,000 square feet, they are required to have man doors installed.

 

There is a provision in NFPA 101 that states the following:

 

7.14.2.2 Egress from normally unoccupied building service

equipment support areas shall be provided by doors complying

with 7.2.1 where the normally unoccupied building service

equipment support area exceeds 90,000 ft2 (8370 m2) in buildings

protected throughout by an approved, supervised automatic

sprinkler system in accordance with 9.7.1.1(1).

 

7.14.2.3 The absence of sprinklers in the normally unoccupied

building service equipment support area, as permitted by

an exemption of NFPA 13, shall not cause a building to be classified

as nonsprinklered for purposes of applying the provisions

of 7.14.2.2.

 

 

I am looking for the exemption in NFPA 13 that would allow a space to have
man-doors, and also allow the sprinklers to be omitted from that space so
that I can apply 7.14.2.3.  Can anyone help by showing me where that might
exist in NFPA 13?  This provision was added to the 2012 edition of NFPA 101.


 

Thanks

 

Pete Larrimer 

VA



-- 
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Covered Parking in 13R

2020-05-29 Thread Art Tiroly via Sprinklerforum
Check with the AHJ. I’m not sure you can change from 13 to 13R in the same 
building. You can use residential rules in a 13 system of course. Do you have 
combustible concealed spaces in the residential?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of 321 via Sprinklerforum
Sent: Friday, May 29, 2020 6:02 PM
To: Art Tiroly via Sprinklerforum
Cc: 321
Subject: Re: Covered Parking in 13R



I think so. I have 2 just like this that I am figuring this way13 R 
upstairs NFPA Parkling downstairs.





John W. Farabee



561-707-5150







On Friday, May 29, 2020, 05:50:22 PM EDT, Art Tiroly via Sprinklerforum 
 wrote:





Residential use above a parking garage changes the occupancy requirement to a 
mixed use and NFPA 13 design criteria is required. Therefore protect the 
garage. Am I on the right track here?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 5:55 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin
Subject: Covered Parking in 13R



I have a 3-story, 13R building. Type IIB construction. On the “engineered” bid 
set, no sprinklers are shown in the covered parking area. This area is inside 
the footprint of the first floor, with 2nd floor units being located above the 
parking area. There are no garage doors and the parking spaces are not 
separated. To sprinkle or not to sprinkle?







John Irwin

West Coast Branch Manager

Quick Response Fire Protection

www.quickresponsefl.com

Office: 844-9QUICKFL

Cell: 727-282-9243

Main Office: 20545 Independence Blvd. Unit G Groveland, Florida 34736

West Coast: 15201 Roosevelt Blvd., Suite 113, Clearwater, Florida 33760

East Coast:   3133 Skyway Circle, Suite 104, Melbourne, Florida 32934

24 Hour Emergency Service Available 1-844-9QUICKFL





“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.” – Benjamin Franklin





  _


 <https://www.avast.com/antivirus> Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com <https://www.avast.com/antivirus>





___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Covered Parking in 13R

2020-05-29 Thread Art Tiroly via Sprinklerforum
Residential use above a parking garage changes the occupancy requirement to
a mixed use and NFPA 13 design criteria is required. Therefore protect the
garage. Am I on the right track here?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 5:55 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin
Subject: Covered Parking in 13R

 

I have a 3-story, 13R building. Type IIB construction. On the "engineered"
bid set, no sprinklers are shown in the covered parking area. This area is
inside the footprint of the first floor, with 2nd floor units being located
above the parking area. There are no garage doors and the parking spaces are
not separated. To sprinkle or not to sprinkle?

 

 

 

John Irwin

West Coast Branch Manager

Quick Response Fire Protection

www.quickresponsefl.com 

Office: 844-9QUICKFL

Cell: 727-282-9243

Main Office: 20545 Independence Blvd. Unit G Groveland, Florida 34736

West Coast: 15201 Roosevelt Blvd., Suite 113, Clearwater, Florida 33760

East Coast:   3133 Skyway Circle, Suite 104, Melbourne, Florida 32934

24 Hour Emergency Service Available 1-844-9QUICKFL

 

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten." - Benjamin Franklin

 



-- 
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR HOSE ALLOWANCE

2020-02-03 Thread Art Tiroly via Sprinklerforum
ESFR hose allowance is 250 gpm.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc. via Sprinklerforum
Sent: Monday, February 03, 2020 6:44 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Trillium Fire Sprinkler Design Inc.
Subject: ESFR HOSE ALLOWANCE

 

I am using Table 16.2.3.1. Nowhere does it state what the hose allowance
requirement is?

I only have 18' storage

It is stated in Table 16.3.3.1 Over 25' storage

 

I know from previous projects it has been 250 gpm but I am just trying to
find it in the code.

 

Any help would be appreciated.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: What storage class is this?

2019-10-31 Thread Art Tiroly via Sprinklerforum
The exposed plastic milk crates drive this into the exposed plastic storage 
hazard.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell









From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Mote via Sprinklerforum
Sent: Thursday, October 31, 2019 12:35 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Richard Mote
Subject: What storage class is this?



Contract documents call out use group classification S-2 Low Hazard Storage 
(46,000SF) This is to be a dry system.



Commodity being stored in a warehouse cooler area min 37° 49' building with 25' 
max storage height, single and multirow racks.
Milk in plastic, glass, or plastic coated paper containers in plastic milk 
crates on wood pallets. And eggs in plastic or pulp paper egg cartons in 
cardboard cartons on wood pallets. None of the pallets are supposed to be 
incapsulated. I've spent several hours looking through the storage chapters and 
can't find a category this fits neatly into.



Richard L. Mote CET

Rimrock Design Services, LLC



--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Underground Sprinkler Lines

2019-03-22 Thread Art Tiroly
My client is on a 5 year plan to replace 75-80 YO cast iron UG fire line that 
is failing.

There is a 5 YO booster pump that churns at 190-200 psi and breaks the sections 
of 5000 Ft. loop.

The new PVC 8” and 10” is holding well once they got the thrust blocks and 
mechanical fittings set properly.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Skyler Bilbo
Sent: Friday, March 22, 2019 5:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Sprinkler Lines



Has anyone installed CPVC piping for an entire fire sprinkler system 
underground?



We are being asked more and more on one story buildings to install wet systems 
where our mains are in the corridor and lines are in the walls.  This involves 
a whole lot of drilling of 2x4's and installing a bunch of protective nailer 
plates (a whole lot of man hours).



Seems to me like we could do it faster using a trencher, installing the vast 
majority of the piping underground with stub ups into the walls for sidewalls.  
I suppose in order to do this correctly, we would have to install a drain, 
perhaps by stubbing into a sump pit somewhere?



I know I have seen a small amount of CPVC piping installed underground in 
apartments that have open stairwells between units, and those don't have a way 
to drain the underground portion, even though this would be after the riser 
controls and fall under NFPA 13(R).



I'm really interested to know if anyone has done it, and/or if there are any 
big reasons not to.  To my knowledge, this isn't specifically addressed in our 
standards.





Thanks,


Skyler Bilbo

217-819-6404 Cell



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Well Water - Raw or non-raw

2019-02-04 Thread Art Tiroly
Would the well be considered as potable drining water?

Particulates are the problem.

If the well draws on a lot of sand it is likely raw water.

What is the likelihood of particulates plugging a 1" sprinkler?

You could add a strainer to remove particulates.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, February 04, 2019 5:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Well Water - Raw or non-raw

 

Would a well be considered a raw or non-raw water source?  We have a project
close by a river that will need a water supply other than the municipal
supply (it is not sufficient).  The system will be an ESFR system, so if the
well is considered raw, then each sprinkler would need return bends and that
is going to be prohibitive. 

 

 <http://www.mfpdesign.com/> MFP_logo_F

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Storage Occupancy - Pipe Schedule

2019-01-16 Thread Art Tiroly
I recently did a system upgrade of an OH pipe schedule system with 130
SF/head..

Good water supply and  a low storage height made it work easily.

Back then only hazardous liquids were designed to extra hazard pipe schedule
and K8 - 90 SF/head.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Spencer Tomlinson
Sent: Wednesday, January 16, 2019 5:26 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Storage Occupancy - Pipe Schedule

 

All - I have a unique situation, unique to me anyway.  Pipe schedule storage
occupancy installed per the 1969 edition of NFPA 13.  It looks to me that
NFPA 231 didn't come out until 1972, meaning storage would have fallen under
what I assume was one of the extra hazard curves in NFPA 13 in 1969 (unless
I'm missing something or misinterpreting this, I have a copy of neither but
would greatly appreciate anyone who may have access sharing).  NFPA 13, 2016
edition will allow for the use of a pipe schedule extension of an existing
"extra hazard" system per 11.2.2.3(2).

 

I have hydraulically calculated the extension, and it results in huge
piping.  Which is fine, but there may be an argument by others that pipe
schedule would be allowed.

 

Now, I know that it is certainly not the best approach - but that aside -
has anyone run into an instance such as this where the pipe schedule
extension has been allowed/approved?

 

Thanks to all in advance.

 

Spencer Tomlinson

Principal, PE

 

red logo

Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com <http://www.tomlinsonfire.com/> 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Indoor Trampoline Park

2019-01-03 Thread Art Tiroly
Due to the change of occupancy the sprinkler system should match the
requirements of the new occupancy.

If quick response sprinklers are required for code compliance then they need
to be changed.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Thursday, January 03, 2019 4:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Indoor Trampoline Park



Some versions of this discussion have come up over the past weeks. We’re
having a bit of an issue with an AHJ in converting a Sports Authority to in
indoor park. Originally we submitted as Light Hazard because it’s an
assembly occupancy. I didn’t necessarily agree with this but … anyway …



The AHJ then wanted all sprinklers changed because they are 286° sprinklers
and thus, not permitted in LH.



So I spoke to said AHJ and told him I really felt this should be at least an
OH occupancy anyway, because of the miscellaneous foam padding and plastics.
He agreed (of course verbally and not in writing). We made those changes and
a couple more he asked for and thought we were good to go.



Today, we received this notice:





Mr. Irwin,

Just a follow up to our phone call earlier.

Thank you for speaking with me earlier.

The existing Fire Sprinkler System was designed and engineered to protect a
specific hazard for the previous occupancy.

There has been concerns about the potential need for reengineering since the
beginning of this project.

Sprinkler Systems in Assemblies are intended for life safety and are
designed as light hazard occupancies with fast activation per NFPA 13.

The proposed Fire Alarm System does not include smoke protection and will be
primarily activated by the Sprinkler System.

The proposed plans are for ordinary group II hazard with high temperature,
standard response sprinklers.

A delay in activation of the Fire Sprinkler and Fire Alarm Systems, may
result in an adverse effect on life safety.

This delay may increase the amount of fire damage.

Additionally this delay and the proposed 8K sprinklers may increase the
amount of water damage.

Please provide a signed and sealed letter from the Engineer of Record
documenting the effects the proposed fire protection systems will have on
occupant notification, occupant evacuation, life safety, and property
conservation.



Options:



*   The Engineer’s letter adequately documents that life safety will not
be adversely effected.
*   The Engineer’s letter indicates a change in hazard classification
and sprinklers.
*   The Engineer’s letter indicates the addition of full smoke
protection to the fire alarm system.



Please be advised that Engineer’s letter along with the most recent revision
will be will be sent out for a third party review by a Fire Protection
Engineer.



Thank you,



I’d especially like to know what Matt and Pete think about this. The
question is, is it always ok to over protect an occupancy? Assuming this is
a LH assembly (which I don’t agree it is) can I protect per OH if I want to?



As a sprinkler contractor, do I have to take alarm activation in to
consideration at all?



How would you proceed with this?







John Irwin

Quick Response Fire Protection

jir...@quickresponsefl.com

CELL – 727-282-9243





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Parts Mezzanine

2018-11-08 Thread Art Tiroly
What is storage class?

How wide are shelves for picking. Solid shelves?

Are there possible obstructions on the walkways?

How high is each level?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Thursday, November 08, 2018 5:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Parts Mezzanine

 

We have a parts mezzanine that uses pick shelves with grated walkways
between. It is about 130' x 186' with three levels. Aisles are 3'-4".

 

The roof system is ESFR K17 sprinkler heads @ 52psi.

 

I am using FM 8-9 but cannot seem to find what the design criteria for the
mezzanine would be.

 

My first thought was to protect it like a normal storage mezz but the code
makes it look more like in-rack protection.

 

Any opinions out there

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe Sch Water Supplies

2018-10-29 Thread Art Tiroly
This is a 55 year old pipe schedule system 130 SF head. This is a change of use 
and requires a density design.

Existing system does not work hydraulically.

Therefore I am creating a calculated system which requires replacing small pipe 
at end of BL’s with 1.5”.



Is this not necessary?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell









From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Monday, October 29, 2018 6:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pipe Sch Water Supplies



Not sure East you mean:  Not meant fro warehousing but you are converting from 
a F occupancy to warehousing.  Nonetheless,tyhere is no schedule for storage.  
That was deleted many cycles ago.





Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/>



Fire Sprinklers Saves Lives









On Oct 29, 2018, at 2:32 PM, Art Tiroly  wrote:



What is the sprinkler spacing 90-130 SF?

Light or OH?



Not meant for warehousing.

I'm working on one now converting from factory to warehousing.

1”, 1”, 1-1/4” does not calculate at 130 SF/head.

Up sizing to get .20/1500 for 8-10’ storage of household furnishings and 
storage.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [ <mailto:sprinklerforum-boun...@lists.firesprinkler.org> 
mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark Eckard
Sent: Monday, October 29, 2018 4:48 PM
To:  <mailto:sprinklerforum@lists.firesprinkler.org> 
sprinklerforum@lists.firesprinkler.org
Subject: Pipe Sch Water Supplies



I remember in some of the older NFPA-13s there were minimum water supply 
requirements for Pipe Scheduled systems.  Does any one have that information?  
I thought I had it, but I cant seem to locate it.



Thank You



Mark E. Eckard SET



Fire Protection Services, LLC

2126 US Hwy. 41 North

Perry, GA 31069

Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta)

Mobile: 478-244-6653

SYL-216






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com

___
Sprinklerforum mailing list
 <mailto:Sprinklerforum@lists.firesprinkler.org> 
Sprinklerforum@lists.firesprinkler.org
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe Sch Water Supplies

2018-10-29 Thread Art Tiroly
What is the sprinkler spacing 90-130 SF?

Light or OH?



Not meant for warehousing.

I'm working on one now converting from factory to warehousing.

1”, 1”, 1-1/4” does not calculate at 130 SF/head.

Up sizing to get .20/1500 for 8-10’ storage of household furnishings and 
storage.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark Eckard
Sent: Monday, October 29, 2018 4:48 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Pipe Sch Water Supplies



I remember in some of the older NFPA-13s there were minimum water supply 
requirements for Pipe Scheduled systems.  Does any one have that information?  
I thought I had it, but I cant seem to locate it.



Thank You



Mark E. Eckard SET



Fire Protection Services, LLC

2126 US Hwy. 41 North

Perry, GA 31069

Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta)

Mobile: 478-244-6653

SYL-216





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

2018-10-09 Thread Art Tiroly
Can the ESFR's be left in place and just add in rack sprinklers as needed?

 

Art

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery
Sent: Monday, October 08, 2018 7:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

 

I think you're right. It just doesn't seem like that should be the case. How
can this spacing allowance be appropriate for the notoriously unforgiving
ESFR criteria, but somehow not OK for the traditionally much more forgiving
standard spray sprinklers. Or that Factory Mutual, who you could say has
more "skin in the game" than NFPA, would allow it if it were a poor
practice. You know what I'm saying?

 

Do you guys think that this spacing arrangement is intentionally prohibited
by NFPA 13, or that it's more of a scenario that just isn't specifically
addressed? In other words, does anyone think that a sprinkler system with
standard spray heads spaced at 10, 10, 9, 11, 10, 10, 9, 11 (per ESFR
requirements) would actually be deficient as a result? I'm thinking about
taking this to the AHJ to see if they would allow it, but I don't want to
suggest doing it if there is good reason to believe that it is a "bad fire
protection practice".

 

I appreciate the input.

 

Kyle Montgomery

 cid:image001.gif@01CAA0CE.8D8066F0

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

 <mailto:kmontgom...@aerofire.com> kmontgom...@aerofire.com

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of MFP Design, LLC
Sent: Monday, October 8, 2018 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues

 

FM allows it because all of their sprinklers are "storage" sprinklers.  It
doesn't matter if it is CMDA, CMSA or ESFR, it is a "storage" sprinkler for
FM so the extended requirements are in play.  I don't think you will find
any forgiveness on this issue in 13.

 

Every time we've dealt with this in the past, we have had to respace
sprinklers along the branchline when that happens.

 

MFP_logo_F

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

 

http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign 

LinkedIn: https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

From: Sprinklerforum  On
Behalf Of Kyle.Montgomery
Sent: Monday, October 8, 2018 1:26 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Converting from ESFR to CMDA - Spacing Issues

 

We're looking at a project where a portion of an existing ESFR building is
being converted to store cartooned expanded plastics. It looks like we've
settled on a design criteria that involves changing out the sprinklers at
the deck to 11.2K standard spray sprinklers at a 0.45 density and adding 2
levels of in-rack sprinklers.

 

This issue I need to address is this: Existing ESFR sprinklers took
advantage of the spacing allowance to avoid being obstructed by structural
members. The lines are 10 ft on-center and the head spacing is 10, 10, 9,
11, 10, 10, 9, 11.

 

The new upright sprinklers are limited to 100 square foot maximum spacing.
Is there any good option/allowance where we could just replace the heads and
keep the spacing? Or are we going to need to relocate every fourth head to
maintain 10-foot spacing all the way down the branch line.

 

I'm pretty sure FM Global allows for this, but I haven't found anything in
NFPA 13 outside of the ESFR section. It sure seems like if it's appropriate
for ESFR heads (arguably the most finicky with regard to
spacing/obstructions) that the same spacing should be OK for standard spray
sprinklers.

 

Kyle Montgomery

 cid:image001.gif@01CAA0CE.8D8066F0

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

 <mailto:kmontgom...@aerofire.com> kmontgom...@aerofire.com

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinkler heads popping off randomly

2018-09-13 Thread Art Tiroly
If the fusible link flies apart it is due to heat.

High pressure can cause a head to leak but not open the link.

Sprinklers with fusible links can slowly melt or creep then the link will 
eventually open.

There must have been excessive heat at the roof at various times.

I would check sprinklers head links near those that actuated.

Links will start to fail with the link solder cracking





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Thursday, September 13, 2018 5:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly



Probably a buildup of pressure from heat rejection off the roof.  Check system 
gauges.  A good pilot operated relief valve would open to relieve and close.



From: Sprinklerforum  On Behalf 
Of Jeff Normand
Sent: Thursday, September 13, 2018 5:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly



Does it only happen in the summertime or hot days?



165 F sprinklers at the roof of a warehouse, this would normally require 200 F 
sprinklers.



That would be my first guess but if it  is only 1 sprinkler at a time, I just 
don't know.



On Thu, Sep 13, 2018 at 4:20 PM Larry Block, Property Manager 
 wrote:

Hi to all!



I manage a number of most warehousing industrial parks around Los Angeles and 
only 1 of them has a problem with heads popping off for no apparent reason. We 
really need some help here in identifying the cause and its correction. Many 
have said to just replace them but who is to say that this will not happen 
again soon, if not later. The facts:



1. Concrete tilt up bldg from 1967 with its roof at 20’ H.

2. Heads are Reliable model C with the fusible link

3. Heads will get the 50 year  UL testing in 4 years (though I assume the 
165degF rating is not relevant here)

4. We have lost 7 heads over 15 years, with 3 in the last 4 months!

5. The link assemblies are never found but the remaining “rings” show no 
issues. The bronze seats

of the head’s  water port are always in perfect condition.

6. We see that the head’s “knuckle” that is opposite the fusible link is 
usually perfectly aligned,

  but a few of them are offset up to a 1/16” and it appears that 
when they move like that,

they are rotating in an arc from the pivot points .

7. The water utility swears that at the time of these events, there are no 
pressure surges.

8. No more than one head has ever gone off at a time and are not just at one 
location or riser.

9. A nearby similar bldg of ours  from 1968 with the same heads has never had 
one such event.



We have entertained the possibility of water pressure, birds, electrolysis, 
dezincification, vibration and are at a loss.



Any helpful thoughts?



Thanks,



Larry Block, Property Manager






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>
 Image removed by sender.

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No Jockey Pump

2018-08-29 Thread Art Tiroly
What is city water static pressure?

 

What is the pressure when pump is running?

 

Likely an omission by installer.

 

Could it have been removed?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Thomas Reinhardt
Sent: Wednesday, August 29, 2018 5:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: No Jockey Pump

 

Hi group,

Found a 50 yr. old fire pump at a business that didn't have a jockey pump.
Am I missing something. Thanks

 

Tom Reinhardt

Fire Inspector/Plan Reviewer

Skokie Fire Department 

7424 Niles Center Road

Skokie, IL 60077

Office: 847-982-5342

thomas.reinha...@skokie.org

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Self storage warehouses

2018-07-26 Thread Art Tiroly
They will allow car storage with fuel in the tank.

Metal partitions will easily transmit heat to the adjacent unit.

No propane tanks.

Corp allowed to store overflow stock or equipment.

40,000 SF in low bay.

Corridors will have drop ceilings with pendant sprinklers.





Art Tiroly

ATCO Fire Protection

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Thursday, July 26, 2018 3:39 PM
To: Sprinklerforum
Subject: Re: Self storage warehouses



Make sure they have restrictions on things like rubber tires, flammable 
liquids, etc.


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)






On Jul 26, 2018 at 3:31 PM, mailto:atir...@atcofirepro.com> > 
wrote:

Storage units 200 -600 SF per unit covered by metal screen at 10 Ft. AFF with 
metal sided partitions.

Household goods, mattresses, foam  cushions on sofas. Class 3-Class A plastic.

Roof sprinklers at 14FT is a pipe schedule system from 1956.

This is a change of occupancy.



The existing pipe schedule system is not adequate for the hazard.

The sprinkler system should be revised and brought up to NFPA design density.

Is the appropriate design based on Class A plastic or something less?

I could not find anything in archives.



Art Tiroly

ATCO Fire Protection

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com

___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Self storage warehouses

2018-07-26 Thread Art Tiroly
Storage units 200 -600 SF per unit covered by metal screen at 10 Ft. AFF
with metal sided partitions.

Household goods, mattresses, foam  cushions on sofas. Class 3-Class A
plastic.

Roof sprinklers at 14FT is a pipe schedule system from 1956.

This is a change of occupancy.

 

The existing pipe schedule system is not adequate for the hazard.

The sprinkler system should be revised and brought up to NFPA design
density.

Is the appropriate design based on Class A plastic or something less?

I could not find anything in archives.

 

Art Tiroly

ATCO Fire Protection

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Misc Rack Storage

2018-05-17 Thread Art Tiroly
Two rows of in-rack sprinklers may solve the rack problem.

 

Art Tiroly

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Thursday, May 17, 2018 11:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Misc Rack Storage

 

Regardless of the trailers, do I need to provide .6/2000 for the racks? If so, 
do I need to do that for the entire 5,000 sqft area? Seems excessive. 

 

 

 

John Irwin

DynaFire Inc. – “Same Day – Next Day”

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Steve 
Leyton
Sent: Thursday, May 17, 2018 11:19 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Misc Rack Storage

 

I tend to agree – trailers potentially shielding fire load within from 
sprinklers above (5.4.2).

 

SL 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Thursday, May 17, 2018 7:06 AM
To: Sprinklerforum
Subject: Re: Misc Rack Storage

 

Wouldn’t the trailer storage bring it up to EH2?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)

 

On May 17, 2018 at 9:47 AM, mailto:john.ir...@dynafire.com> > 
wrote:

Here’s the situation … I have a 5,000 sqft, (currently) ordinary hazard mixed 
use space. The new tenant intends to store two emergency disaster management 
trailers in this space. However, along two walls, they want to put a 3-teir 
rack with storage up to 20’ in height. TOS in the center of the unit is 23-9.

 

The racks will contain a mix of group A plastic, emergency supplies in plastic 
totes, with lids, on non-combustible pallets. 

 

Do I really have to upgrade this entire space from OH II to .6/2000?

 

Do I tell them they should just not store over 12’?

 

John Irwin

Fire Sprinkler Specialist

DynaFire, Inc. – “Same Day – Next Day”

727-282-9243 – Cell

 

“A customer is the most important visitor on our premises. He is not dependent 
on us. We are dependent on him. He is not an interruption on our work. He is 
the purpose of it. He is not an outsider on our business. He is a part of it. 
We are not doing him a favour by serving him. He is doing us a favour by giving 
us an opportunity to do so.”

 

 

___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: main drain flows

2018-04-26 Thread Art Tiroly
What is the fire flow test for this system?

What size is the underground fire line.

What size is the riser to be.?



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 5:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: main drain flows



They are looking for the GPM flows out of our main drain during a main drain
tests. Since a lot of water is going to be released during the test they
want to make sure the sanitary sewer can handle all the water with the main
drain fully open under city pressure.



Tony





From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Steve Leyton
Sent: Thursday, April 26, 2018 1:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: main drain flows



Tell them you want a hub drain with a self-priming 4” trap.  It’ll resolve
both 1¼” and 2” main drain discharges.



Steve



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tony Cetani
Sent: Thursday, April 26, 2018 1:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: main drain flows



Long time reader, first time writer…..actually not that long I’m a fairly
new designer. We have a jurisdiction where they require the main drain to
drain to a sanitary sewer and the contractor is asking what the flows will
be so they can size their SS line accordingly. The sprinkler system hasn’t
been designed yet and they said they need to know right now so they can
finish their design and submit for permit. Is there a way to figure this out
(or get a ball park) just based off city water flow numbers?



Thank you



Tony









---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Special Designs of Storage Protection Section 20.5 (2013 ed.)

2018-04-03 Thread Art Tiroly
Are the aisles narrow like 30-48”?

The cat walks are likely considered obstruction to the ESFR roof system.

Therefore QR sprinklers are required below the cat walks.

See Section 20.7.3. for ESFR. Does this qualify with these 10 requirements?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Zachary Siegrist
Sent: Tuesday, April 03, 2018 4:34 PM
To: Sprinklerforum@lists.firesprinkler.org
Subject: Special Designs of Storage Protection Section 20.5 (2013 ed.)



All,

I am an AHJ and was called to inspect a installation for protection of carton 
record storage for a single- level catwalk.  The existing ceiling level 
protection is an ESFR system.  Section 20.5.6.2.1 states that ceiling 
sprinklers spaced to cover a maximum of 100 SF shall be standard response spray 
sprinklers with K-factors per Section 12.6.  Is this explicitly stating that 
there can't be an ESFR system at the deck level (35 feet AFF) b/c of its fast 
response element?   Does Section 12.6.6 make this permissible?  Appreciate any 
feedback I can get.



Zach



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: PVC drain line

2018-03-31 Thread Art Tiroly
Creating a PVC drain header for the branch lines should not be done.

Same reason as not running PVC with sprinkler head tees. Not an approved
material.

 

Art Tiroly

ATCO Fire Protection

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Scott Futrell
Sent: Friday, March 30, 2018 6:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC drain line

 

Yes, I do think that is the way to go, but it is a sprink contractor making
the suggestion. I'm trying to justify a response one way or the other.

 

Scott

 

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of MFP Design, LLC
Sent: Friday, March 30, 2018 5:17 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: PVC drain line

 

I thought I was going to be called crazy for suggesting a valve at the end
of each line and then running it in PVC.  It would be expensive for sure.
Let me know if you are going to go that way and I will be stock in the valve
suppliers.

 

Practically, run it in steel and call it good.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi
gn.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4
2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2
FYfycgtd5nsFrrpvzulZiNkQ%3D=0> http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo
ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b
4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166
77342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of
Matthew J Willis
Sent: Friday, March 30, 2018 3:13 PM
To: Forum <sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> >
Subject: RE: PVC drain line

 

So,

The answer would be no. Right?

Plastic is fine for drain, not listed. But all piping before the valve is.

 

R/

Matt

 

Sent from my Verizon 4G LTE Droid

On Mar 30, 2018 4:10 PM, Scott Futrell <sco...@ffcdi.com
<mailto:sco...@ffcdi.com> > wrote:

I can't see a valve at the end of each line being practical.  Then you'd
need a lift to drain them when you wanted to use it and these are >25K
square foot systems, so many valves.

 

Scott

 

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jeff Normand
Sent: Friday, March 30, 2018 5:07 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Re: PVC drain line

 

I say it's fine if you have drain valves at the end of each line and
transition to pvc after the valve. But that may be expensive. 

 

So I say pvc is ok after the drain valve.

 

But is that practical?

 

On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell <sco...@ffcdi.com
<mailto:sco...@ffcdi.com> > wrote:

A Friday afternoon conundrum for the group.

 

I have a client with corrosion issues in several wet, twenty year old, ESFR,
warehouse systems.  These are center-fed systems.  Yes, center-fed. So all
of the branchlines are dead ends.  Corrosion scale and sludge is pushed into
the ends of the lines.  Flushing will be done.  End of the day though the
client wants to add a tie-in drain line connecting all the ends of all the
lines to drain/flush in the future.  It has been suggested that schedule 40
PVC might be used for these tie-in drains.

 

My response so far:

 

Practically, plastic should be okay.

 

But, it would not be recognized in NFPA 13.  Also, because it could fail in
a fire, and we would expect high challenge fires in warehous

RE: Butane

2018-03-20 Thread Art Tiroly
How is the butane contained In steel high pressure cylinders or something
larger?
If the vessels are kept cool with water spray during a fire then it is safe.
Leaks could have flash or explosion hazards potential.
Need more info.


Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Tuesday, March 20, 2018 3:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Butane

I am looking at a space for a client that want to store butane, a lot of
butane.

 

I have been looking through NFPA #30 & #32 for some guidance but I am still
unsure, as one of the MSDS sheets says to protect it as outlined in NFPA #30
but my brain is saying it is more like a Level 3 Aerosol.

 

The building is protected with ESFR K17 @ 35psi

 

Any words of wisdom out there?

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20180320/15b72ced/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Residential Sprinklers

2018-03-05 Thread Art Tiroly
Using 5.6K QR heads will change the hydraulic calculations and minimum flows
allowed by residential sprinklers.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Reed A. Roisum, SET
Sent: Monday, March 05, 2018 4:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Residential Sprinklers

Are residential sprinklers required for dwelling units in NFPA 13R?  It
appears as though they can be QR or residential in the 2012 IBC (903.3.2).
For some reason I had in my mind that they needed to be residential within
the dwelling unit or sleeping unit??

Thanks.

Reed R.

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
http://www.kfiengineers.com


__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Tire Storage

2018-02-23 Thread Art Tiroly
I believe that means a HE foam system plus a sprinkler system with a .30
density.


Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tony Silva
Sent: Friday, February 23, 2018 3:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Tire Storage

NFPA 13, 2014 Table 18.4(a)

Some "Sprinkler Discharge Densities" are given as (for example):

"0.30 plus high expansion foam"

Does this mean the roof system needs to be high expansion foam with a
density of 0.3? I'm just confused with the use of the word "plus" and want
to make sure it doesn't mean anything else.

Thanks,

Tony
-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20180223/131521aa/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Apartment Crawl Space

2018-01-11 Thread Art Tiroly
Check out the residential rules in NFPA 13, Section 8.4.5. Similar to 13-R.
4 heads.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, January 11, 2018 2:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Apartment Crawl Space

 

Looking at a (5) story apartment building so I assume it would need to be
per NFPA-13 correct? With that being said is there anything in the Standard
that addresses the crawl space underneath? Concealed Space?

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: High-Rise with Secondary Water Supply

2017-12-06 Thread Art Tiroly
In our jurisdiction the backflow would be required where it enters the building 
from underground.

A long run of black steel pipe is not allowed without a BFP assembly.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Kyle.Montgomery
Sent: Wednesday, December 06, 2017 3:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: High-Rise with Secondary Water Supply



I’m working on a high-rise that has two water supply lead-ins. One comes in 
adjacent to the pump room, but the secondary supply has to run 200+ feet 
through the building. The plan was to have the backflow preventors in the fire 
pump room. Am I violating any code requirements and/or good design practices by 
doing this? (Note: I know that I’ll need an appropriate distance between the 
backflows and the pump suction and/or to use OS valves).



A couple of potential concerns have been raised:



1.  200-plus feet of “unmonitored” pipe running through the building. I 
guess there is some concern you could have a leak and not have any kind of 
alarm. Is there any code requirement to have a flow switch within a certain 
distance from where the water supply enters the building?

2.  Are there specific code requirements for the pipe type between the 
underground lead-in and the backflow prevention device? We’ve been asked to 
provide galvanized pipe in similar scenarios before, but it was suggested that 
that might not be AWWA-compliant.



Thanks for your input.



Kyle Montgomery

 cid:image001.gif@01CAA0CE.8D8066F0

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

kmontgom...@aerofire.com







---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC sizing on wet automatic standpipes

2017-11-17 Thread Art Tiroly
Is this a residential or light hazard 8 story building?

Do you have a 1000 gpm fire pump from city water? Electric or diesel?

Reliable power with no outages?

3 - 4 or more standpipe risers?



Then you can get answers.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ben Young
Sent: Friday, November 17, 2017 11:05 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC sizing on wet automatic standpipes



I'm not lucky enough to be able to treat the FDC on a wet automatic standpipe 
as supplemental am I?

We have a building with a combined sprinkler and standpipe system that's wet 
automatic. Building is 8 stories, but separated. etc. etc.

Since the standpipe is wet automatic, the FDC isn't the only supply source, so 
do we still have to calculate it hydraulically? Total standpipe demand is 1000 
GPM

We're using NFPA 14, 2013 edition.



Basically, I'm trying to figure out if its OK to run 4" to the FDC and use a 
single Siamese instead of 6" piping to a 4-way or two Siamese connections.



Benjamin Young



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: lag bolts

2017-10-25 Thread Art Tiroly
Trapeze to spread the load?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: lag bolts



Sorry I should have clarified, this is for hangers not EQ bracing



Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





roc...@norcalfire.com

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mitchell, Scott
Sent: Wednesday, October 25, 2017 10:24 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: lag bolts



Through bolt?



J. Scott Mitchell, PE

Senior Fire Protection Engineer

Mission Engineering

CNS Y-12 | 865-576-5258

CNS PTX | 806-477-5883

thMYA3SSEP





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: lag bolts



NFPA 13 9.1.5.3.2 states that if 2½” long screws can’t be used then 2” can
but spacing can’t exceed 10’….what’s one to do if 3” lags can’t be used? We
have a 6” main and only 2½” x 12” wood joists to attach to.



Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III



Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590





roc...@norcalfire.com

www.norcalfire.com <http://www.norcalfire.com/>



CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Parking Under MTA Tracks

2017-06-29 Thread Art Tiroly
An recent arson car fire beneath a bridge structure caused the collapse of the 
steel structure and bridge deck on I-85 in Atlanta.

It will take months to repair.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Thursday, June 29, 2017 2:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Parking Under MTA Tracks



That is an approach I never thought of, I focused on the tracks and not the 
concept of the structure.  Like you said , I am not sure what occupancy group 
it would fall under, but technically a structure no different than any other 
building.



Mike Stossel SET

400dpiLogoCropped

36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

m...@knssprinkler.com



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Wayne Cordiner
Sent: Thursday, June 29, 2017 2:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Parking Under MTA Tracks



Mike,



NYC BC 903.2.10.3 Parking Garages, states an automatic sprinkler system shall 
be provided throughout buildings classified as enclosed parking garages in 
accordance with section 406.4 or where open or enclosed parking garage is 
located beneath other occupancy groups.

I wish I could tell you which occupancy group elevated train tracks fall under 
but regardless the only exception is an R-3 so automatic sprinklers appear to 
be required.

I've attached a link to the BC site. Hope this helps.



https://www1.nyc.gov/site/buildings/codes/2014-construction-codes.page

Regards,



Wayne T. Cordiner, Jr.

917-426-5844




On Jun 27, 2017, at 19:22, Mike Stossel <m...@knssprinkler.com> wrote:

Does anyone know of an NFPA code that addresses parking under train tracks?  I 
have a customer in New York City that is going to rent the space under the 
tracks for parking.  One of the requirements that New York City has made is 
that proper fire protection is provided, but gave no indication as to what this 
is.  I checked NFPA 130 thinking that standpipes maybe required, but I could 
not find any information pertaining to this scenario.  Any ideas or direction 
is greatly appreciated, and thank you in advance for the help.







Mike Stossel SET



36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

m...@knssprinkler.com



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
About 4000 Ft. of pipe, 300 sprinklers.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Tuesday, June 13, 2017 6:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.



Well, one thing is for sure, your customer would be on AEP’s (American Electric 
Power) Christmas card list the first time they powered the trace system up! 
Hundreds of feet of resistance heating cable…what a “peak” demand that would 
set.



John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: Tuesday, June 13, 2017 6:25 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Heating cable and 1" wrap.



Yeah...I had some one tell me it was like $5/ft for the materials.  Now, using 
Professor Greenman's qualitative formula, it would be about $10/ft + all the 
extras :-) I don't know how accurate or not, but that sure would keep me from 
doing an entire system in it.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 6/13/2017 3:08 PM, rongreenman . wrote:

Just figure a lot per foot, double it, and then add on the extras.



On Tue, Jun 13, 2017 at 3:05 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Thanks.

How do you determine the cost of operating a heat trace system?

That is important to convey



Ary



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Normand
Sent: Tuesday, June 13, 2017 5:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Heating cable and 1" wrap.



If ceiling is too costly wait until you see the price of heat tracing an entire 
system.







On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

They need store packaging material, idle pallets.



Ceiling is also too costly.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.



What are they storing?



Could they put in a false ceiling?



Matt





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Heating cable and 1" wrap.



I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.



Dry system requirements for solid piled storage over 25Ft high in 35 Ft. high 
building are not available.



I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the 
sprinkler pipe with heat cable and 1” insulation.

This method is in 13. Tyco has a system to apply heating cable to branch lines 
and cross mains.



In over 50 years I have never seen or heard of heat tracing being done. I think 
it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a sprinkler 
system.



What arguments can I use to avoid this method of keeping a wet grid system from 
freezing.







Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899 <tel:%28216%29%20621-8899>

216-570-7030 <tel:%28216%29%20570-7030>  cell






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>
 Image removed by sender.

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







--

Ron Greenman


rongreen...@gmail.com

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)





___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses

RE: Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
Thank you for all your comments.

I want to get this building heated and not do a heat trace system.



I will keep fighting to keep them from making this mistake.

I have offered them an HVAC PE to do a work up but they don’t want to spend the 
money.

They don’t like engineers or construction managers.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell









From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: Tuesday, June 13, 2017 6:25 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Heating cable and 1" wrap.



Yeah...I had some one tell me it was like $5/ft for the materials.  Now, using 
Professor Greenman's qualitative formula, it would be about $10/ft + all the 
extras :-) I don't know how accurate or not, but that sure would keep me from 
doing an entire system in it.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 6/13/2017 3:08 PM, rongreenman . wrote:

Just figure a lot per foot, double it, and then add on the extras.



On Tue, Jun 13, 2017 at 3:05 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Thanks.

How do you determine the cost of operating a heat trace system?

That is important to convey



Ary



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Normand
Sent: Tuesday, June 13, 2017 5:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Heating cable and 1" wrap.



If ceiling is too costly wait until you see the price of heat tracing an entire 
system.







On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

They need store packaging material, idle pallets.



Ceiling is also too costly.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.



What are they storing?



Could they put in a false ceiling?



Matt





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Heating cable and 1" wrap.



I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.



Dry system requirements for solid piled storage over 25Ft high in 35 Ft. high 
building are not available.



I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the 
sprinkler pipe with heat cable and 1” insulation.

This method is in 13. Tyco has a system to apply heating cable to branch lines 
and cross mains.



In over 50 years I have never seen or heard of heat tracing being done. I think 
it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a sprinkler 
system.



What arguments can I use to avoid this method of keeping a wet grid system from 
freezing.







Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899 <tel:%28216%29%20621-8899>

216-570-7030 <tel:%28216%29%20570-7030>  cell






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







--

Ron Greenman


rongreen...@gmail.com

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)






___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
Thanks.

How do you determine the cost of operating a heat trace system?

That is important to convey



Ary



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Normand
Sent: Tuesday, June 13, 2017 5:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Heating cable and 1" wrap.



If ceiling is too costly wait until you see the price of heat tracing an entire 
system.







On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

They need store packaging material, idle pallets.



Ceiling is also too costly.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.



What are they storing?



Could they put in a false ceiling?



Matt





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Heating cable and 1" wrap.



I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.



Dry system requirements for solid piled storage over 25Ft high in 35 Ft. high 
building are not available.



I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the 
sprinkler pipe with heat cable and 1” insulation.

This method is in 13. Tyco has a system to apply heating cable to branch lines 
and cross mains.



In over 50 years I have never seen or heard of heat tracing being done. I think 
it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a sprinkler 
system.



What arguments can I use to avoid this method of keeping a wet grid system from 
freezing.







Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell






 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>
 www.avast.com




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
What about using Single Interlock Pre-action.

 

We got a bid for a "Quell" pre-action dry system with detection that is
crazy expensive with a 2500 gpm fire pump.

Good city water is adequate for an ESFR system without a pump from a 20"
water main.

 

What is the poor reliability aspect Concern?

 

Art

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, June 13, 2017 5:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.

 

?  You could use heat detection in lieu of smoke detection depending on
environmental conditions.  

 

Heat tracing a complete system is a disaster waiting to happen IMHO.  

 

Also the Heat trace system must be electronically supervised to insure
operability.  So he will need a fire alarm system for it to connect to.  

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
craig.pr...@ch2m.com



 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 4:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Heating cable and 1" wrap. [EXTERNAL]

 

I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.

 

Dry system requirements for solid piled storage over 25Ft high in 35 Ft.
high building are not available.

 

I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the
sprinkler pipe with heat cable and 1" insulation.

This method is in 13. Tyco has a system to apply heating cable to branch
lines and cross mains.

 

In over 50 years I have never seen or heard of heat tracing being done. I
think it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a
sprinkler system.

 

What arguments can I use to avoid this method of keeping a wet grid system
from freezing.

 

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=link> www.avast.com 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
They need store packaging material, idle pallets.

 

Ceiling is also too costly.

 

Art

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Heating cable and 1" wrap.

 

What are they storing?

 

Could they put in a false ceiling?

 

Matt 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Heating cable and 1" wrap.

 

I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.

 

Dry system requirements for solid piled storage over 25Ft high in 35 Ft.
high building are not available.

 

I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the
sprinkler pipe with heat cable and 1" insulation.

This method is in 13. Tyco has a system to apply heating cable to branch
lines and cross mains.

 

In over 50 years I have never seen or heard of heat tracing being done. I
think it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a
sprinkler system.

 

What arguments can I use to avoid this method of keeping a wet grid system
from freezing.

 

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=link> www.avast.com 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Heating cable and 1" wrap.

2017-06-13 Thread Art Tiroly
I have a client that is renovating an uninsulated 30,000 SF shed warehouse.

He does not want to heat the building.

 

Dry system requirements for solid piled storage over 25Ft high in 35 Ft.
high building are not available.

 

I am pushing for an ESFR wet system in a heated building.

Rather than heating an uninsulated building owner suggests we heat the
sprinkler pipe with heat cable and 1" insulation.

This method is in 13. Tyco has a system to apply heating cable to branch
lines and cross mains.

 

In over 50 years I have never seen or heard of heat tracing being done. I
think it is a mistake due to reliability and cost

There must be reasons this heating method is not being installed on a
sprinkler system.

 

What arguments can I use to avoid this method of keeping a wet grid system
from freezing.

 

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pump pads

2017-06-12 Thread Art Tiroly
I saw it done some years ago by pipe fitters and it made me laugh.

The fittings were below the concrete floor so they gouged to floor for the 
flanges.

If you need to go back underground the ell won’t fit  at the floor.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: Monday, June 12, 2017 12:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Pump pads



We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.



What say you?







John Irwin

Division Manager - Fire Sprinklers

Critical System Solutions

jir...@criticalsystemsolutions.com

813-618-2781





Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Steam Driven Fire Pumps

2017-05-24 Thread Art Tiroly
I have seen a seen steam turbine driven fire pump about 30 years ago.

Call a fire pump rep and they should know.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: Wednesday, May 24, 2017 3:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Steam Driven Fire Pumps

 

A building owner needs a fire pump and would like steam driven.

 

Are these even made/approved anymore, for new installations?

 

thanks in advance!

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

bcasterl...@fsc-inc.com

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dip tanks

2017-05-02 Thread Art Tiroly
A safer solvent wash tank would have an automatic closing lid actuated by a
fusible link.

Would a Stoddard solvent with a flash point over 100*F be acceptable?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Tuesday, May 02, 2017 3:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Dip tanks



I have been looking through NFPA #34 (2007) to find out if there is a
minimum or maximum size for a dip tank and the requirements for them



We have a client with a small dip tank for cleaning parts prior to powder
coating, the tank holds less than 2 gallons of flammable liquid and has a
surface area of less than 2 ft². The tank is metal and has a lid when not in
use. The tank is in a ventilated area, inside a paint booth.



This is a small operation and the bake oven is also in the paint booth, the
concern I see is the electrical associated with the bake ovens and the
proximity to the dip tank.



All the dipping is manual. The sequence is dipping, drying, power coating
then baking, like I said small operation



Is there anything I am missing.





Thank you





James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sketching software

2017-04-10 Thread Art Tiroly
You could make PDF's details from AutoCAD drawings to add to documents.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott Futrell
Sent: Monday, April 10, 2017 1:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sketching software

 

Does anyone have suggestions for software to make good, neat, details for
use on a desktop or Android tablet? Not AutoCad or HydraCad, just something
to use to make details to put in reports, letters, presentations.

 

To make details of pipe and fittings both above ground and underground?

 

Thanks in advance,

 

Scott Futrell

Futrell Fire

 

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 20 4.7.7.2

2017-04-06 Thread Art Tiroly
Get a 3000 gpm flow test with multiple hydrants as required. What size is
the city main?

With 180 gpm per head you need bigger pipe to lower pump pressure.

(I do hydraulic analysis to solve problems like this.)

 

Art

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Colin Carew (Cambridge)
Sent: Thursday, April 06, 2017 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2 

 

The system demand is 2210.4 ,  

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: April-06-17 4:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2 

 

You can't use the PRV to relieve excess pressure under normal conditions due
to an over designed pump.  There can be unexpected times in a municipal
supply where pressure spikes occur for various reasons.  If your pump
selection puts you close to the maximum system working pressure under normal
conditions and a spike in the supply were to occur, with no means of relief,
downstream system damage could occur.  

 

 

One other concern over this selection is that it is a 1500 gpm pump with
only a 1583 gpm tested source flow rate.  The pump may not be capable of
reaching the 150 % mark unless you know if the municipal supply can actually
provide more than 1583 gpm.  Not knowing the actual system demands makes it
difficult to address this issue any farther.

 

 

 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
craig.pr...@ch2m.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tom Duross
Sent: Thursday, April 06, 2017 4:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2 [EXTERNAL]

 

Looks like you could be above 200 PSI churn or system pressure.  The
standard (2013 referenced) does not allow you to use the relief as a means
of blowing off excess pressure above 175.

Tom

 

Is the 140 psi total pressure or pump rating?

 

The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.

 

So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.

 

Is this a diesel or electric?

 

How much pressure do you need at these heads?

 


Craig L. Prahl 

 

Hi Forum , 

 

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone . 

 

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being 

Used but 4.7.7.2 is  causing me to scratch my head . 

 

 

Colin 

 

 

 

 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 20 4.7.7.2

2017-04-06 Thread Art Tiroly
The LP-46 only requires 15-20 psi end head.

I don't understand the excessive pressure you require.

The 58/56/1583 is a great suction source.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 06, 2017 4:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2 

 

You can't use the PRV to relieve excess pressure under normal conditions due
to an over designed pump.  There can be unexpected times in a municipal
supply where pressure spikes occur for various reasons.  If your pump
selection puts you close to the maximum system working pressure under normal
conditions and a spike in the supply were to occur, with no means of relief,
downstream system damage could occur.  

 

 

One other concern over this selection is that it is a 1500 gpm pump with
only a 1583 gpm tested source flow rate.  The pump may not be capable of
reaching the 150 % mark unless you know if the municipal supply can actually
provide more than 1583 gpm.  Not knowing the actual system demands makes it
difficult to address this issue any farther.

 

 

 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
craig.pr...@ch2m.com



 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tom Duross
Sent: Thursday, April 06, 2017 4:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 20 4.7.7.2 [EXTERNAL]

 

Looks like you could be above 200 PSI churn or system pressure.  The
standard (2013 referenced) does not allow you to use the relief as a means
of blowing off excess pressure above 175.

Tom

 

Is the 140 psi total pressure or pump rating?

 

The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.

 

So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.

 

Is this a diesel or electric?

 

How much pressure do you need at these heads?

 


Craig L. Prahl 

 

Hi Forum , 

 

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone . 

 

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being 

Used but 4.7.7.2 is  causing me to scratch my head . 

 

 

Colin 

 

 

 

 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Paint Booth Exhaust Stack

2017-03-16 Thread Art Tiroly
Is that the total duct length or is there a riser to the roof?

Are there heads in the plenum behind the filter?

Where is the exhaust  fan?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Thursday, March 16, 2017 4:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Paint Booth Exhaust Stack

 

NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have
sprinklers located on 12'-0" centers beginning no more that 6'-0" from the
duct entrance.

 

If the horizontal run is only 2'-0" do you require a sprinkler head to
protect this section of the duct, (is there a minimum distance)

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Built-up roof deck as a limited-combustible construction

2017-03-10 Thread Art Tiroly
If it is covered with gravel and there is no exposed combustible material then 
could a fire propagate in this concealed space?



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of David Bitton
Sent: Friday, March 10, 2017 5:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Built-up roof deck as a limited-combustible construction



Hello Todd,



The original building plans are not available.  I am considering this to be a 
Class II metal deck roof, and assuming tar and gravel, foam insulation, a 
combustible vapor barrier, and combustible adhesive over a steel deck.



David



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Friday, March 10, 2017 5:00 PM
To: Sprinklerforum
Subject: Re: Built-up roof deck as a limited-combustible construction



Any more details on what the built up roof consists of?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)





On Mar 10, 2017 at 4:57 PM, mailto:dbit...@questlosscontrol.com> 
> wrote:

Hello,



I have a 35 ft high building being built adjacent to a 22 ft high building 
which has a built-up, insulated metal deck roof. The structural engineer has 
devised a sloped "snow shed" between the addition and the lower building in 
order to distribute the increased snow load at this juncture.  This will create 
an inaccessible concealed space on the roof which will be of noncombustible 
construction, with the exception of its base, which will be the built-up metal 
deck roof of the existing building.  Would you consider this as meeting the 
definition of "limited combustible construction", meaning that the space would 
not require sprinkler protection?



David Bitton, ing./Eng.


Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, Québec

H4P 1T8



T: (514) 341-4545 C: (514) 996-7483

www.questlosscontrol.com





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Built-up roof deck as a limited-combustible construction

2017-03-10 Thread Art Tiroly
Is it a flat roof?

Is it covered with gravel or stone?

If it is built of felt paper and asphalt/tar it will burn.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell











From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of David Bitton
Sent: Friday, March 10, 2017 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Built-up roof deck as a limited-combustible construction



Hello,



I have a 35 ft high building being built adjacent to a 22 ft high building
which has a built-up, insulated metal deck roof. The structural engineer has
devised a sloped "snow shed" between the addition and the lower building in
order to distribute the increased snow load at this juncture.  This will
create an inaccessible concealed space on the roof which will be of
noncombustible construction, with the exception of its base, which will be
the built-up metal deck roof of the existing building.  Would you consider
this as meeting the definition of "limited combustible construction",
meaning that the space would not require sprinkler protection?



David Bitton, ing./Eng.


Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, Québec

H4P 1T8



T: (514) 341-4545 C: (514) 996-7483

www.questlosscontrol.com





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Size of main service - dry parking garage -

2017-03-04 Thread Art Tiroly
>From the information presented the question can’t be answered.

To do a hydraulic analysis you need:
A water flow test near the point of the connection.

Length of the underground fire main from the connection to the riser.

Elevation of the dry system highest sprinkler.

Is there a fire hydrant supplied from the proposed 4” main?

If yes then the main shall be 6”.



Best analysis is to do a preliminary  hydraulic calculation to determine if 4” 
is adequate.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of very Cool
Sent: Saturday, March 04, 2017 8:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Size of main service - dry parking garage -



Hi:



I am trying to find if a 4" main is adequate for a dry system to serve a 
parking garage.  Here is what I am calculating. Would appreciate any feedback:



The area of application would be 1500 SF, which needs to increase by 30% as per 
Section 11.2.3.2.5, to 1950 SF.



Water demand = 1950  x .15 = 293 GPM

Add 250 hose allowance: 293 + 250=543 GPM

 Velocity at 4" main and 543 GPM =13.7 FPS, therefore ok

Thank you

Ramez









---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Floating Dock

2017-02-16 Thread Art Tiroly
How much movement where dock connects to shore?

Metraflex Co has flex U loop that may be of value.
Can you support pipe on the floor outside the hand rail?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark Phillips
Sent: Thursday, February 16, 2017 4:09 PM
To: sprinklerforum@lists.firesprinkler.org; Charles Thurston
Subject: Re: Floating Dock

Galvanized sch 40
Flexible couplings as it crosses any joints and a thermal expansion join to
land connection.
I think victaulic made one but you coukd make it by using flexible coupling
every six inches on a three foot section



Sent from my Verizon 4G LTE Droid
On Feb 16, 2017 4:02 PM, Charles Thurston <charl...@mbfsg.com> wrote:
Hello Sprinklerforum,

Looking for suggestions for pipe to use on top of a floating dock for the
Manual Dry standpipe. We had pipe under it but due to structural failures of
the dock the pipe is now in 3-5 feet of muck in the bottom of the river.
Looking to run the pipe on top of the dock. There is no access under the
dock. Dock is Aluminum decking welded into place, +/- 185' long, last hose
valve is about 1000 feet from the FDC. Had 6" all the way when it was put in
5 years ago.

--
Best regards,
Charles Thurston
charl...@mbfsg.com<mailto:charl...@mbfsg.com>
MYRTLE BEACH FIRE SAFETY GROUP
A Division of Pye-Barker Fire Safety
1445 Cannon Road
Myrtle Beach, SC 29577
(843) 916 - 8787
(843) 839 - 3473 facsimile

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Commodity class upgrade?

2017-02-11 Thread Art Tiroly
Exposed plastic containers would become Class A exposed plastics in my 
conservative analysis.

They shed water so wetting can’t take place.

How big are the boxes?

Is it a pallet loads of plastic boxes with combustibles. Is it more than 15% of 
the weight of matertials

No access to NFPA today

 

Art Tiroly

ATCO Fire Protection

216-570-7030

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Saturday, February 11, 2017 2:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Commodity class upgrade?

 

I have a project where they are storing class III commodities in plastic totes. 
The product is stored on racks with 12' to top of storage. 

 

Does the plastic totes cause me to increase / modify the commodity class? I 
swear I read something about that in the storage chapters but I can't seem to 
locate it. This jurisdiction is under the 2013 edition of NFPA 13. 

 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Combustible concealed space under stair

2017-02-08 Thread Art Tiroly
Is this an enclosure.

Access door like a closet.?

Electrical equipment?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Wednesday, February 08, 2017 10:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Combustible concealed space under stair



NFPA 13 (07ed) section 8.15.1.2.9



Could this section be applied to a small combustible concealed space under 
stairs that is under 55 SF?

Thanks,

Dewayne





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Artifical Turf

2017-02-01 Thread Art Tiroly
ESFR heads require flue spaces 9' apart and no solid shelves.

Solid shelves or no flues may require in-rack sprinkles.

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Tuesday, January 31, 2017 7:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Artifical Turf

 

We are looking at a client the stores artificial turf in rolls and would
like to store on racking.

 

The racking is multi row racking and the turf is made from polyethylene.

 

My first thought is to protect the same as carpet storage, or can it be
protected as non-expanded group ""A" plastics.

 

The existing sprinkler system is ESFR K17 operating at 52 psi.

 

Thoughts

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Floor mounted obstructions - ORDINARY HAZ

2017-01-28 Thread Art Tiroly
Review all the obstruction rules.

It should become clear.

18” from storage to deflector is required.

There are also distance to wall obstructions that may be helpful.

I don’t have 13 available at home.

 

Art Tiroly

ATCO Fire Protection

2126-570-7030

 

: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Saturday, January 28, 2017 12:39 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Floor mounted obstructions - ORDINARY HAZ

 

Jeff:

 

Amen on the “not clearly stated”!  I saw that paragraph, but it appeared to me 
to refer more to obstructions from the ceiling not the floor. I’m trying to 
throw over the top of the partition and it would be nice if NFPA-13 could give 
a spacing table for Ordinary Hazard like it does for “Light Hazard only”. 
That’s the frustrating part, common sense says the same or similar spacing 
would apply, but Ordinary Hazard is not included.

 

Thanks,

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Normand
Sent: Saturday, January 28, 2017 12:32 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Re: Floor mounted obstructions - ORDINARY HAZ

 

Not that clearly stated but here's the NFPA 13 2016 edition

 

 

8.6.5.3.1 Continuous or noncontinuous obstructions that interrupt

the water discharge in a horizontal plane more than

18 in. (450 mm) below the sprinkler deflector in a manner to

limit the distribution from reaching the protected hazard

shall comply with 8.6.5.3.

 

8.6.5.3.2 The requirements of 8.6.5.3 shall also apply to obstructions

18 in. (450 mm) or less below the sprinkler for light

and ordinary hazard occupancies.

 

A.8.6.5.3.3 When obstructions are located more than 18 in.

(450 mm) below the sprinkler deflector, an adequate spray

pattern develops and obstructions up to and including 4 ft

(1.2 m) wide do not require additional protection underneath.

Examples are ducts, decks, open grate flooring, catwalks,

cutting tables, overhead doors, soffits, ceiling panels,

and other similar obstructions.

 

On Sat, Jan 28, 2017 at 11:10 AM, John Paulsen <j...@crwnfire.com 
<mailto:j...@crwnfire.com> > wrote:

I am trying to determine the proper deflector distance from a partition with 
the top located 18” below the sprinkler deflector. This is an Ord Haz Grp II 
Self Storage facility with standard spray QR Tyco TY-FRB TY3131 uprights. Sec 
8.6.5.2 doesn’t give a table like 8.6.5.2.2 which is for Light Hazard only. 

 

If I have to space the heads as if the low partitions went all the way to the 
deck, I will violate the 6’ minimum rule. What am I missing here?   

 

Thanks,

 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Tank Capacity

2017-01-27 Thread Art Tiroly
Hose demand is usually not art of the equation with good city hydrant supply 
available.

If you omit hose than it all works.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dale Wingard
Sent: Friday, January 27, 2017 4:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Tank Capacity



Thanks everyone.  I just thought that it was always an acceptable practice.



The situation is I have a new owner of a warehouse with an existing ground tank 
and pump house.  We will be replacing the pump.  The tank is only 3000 gallons 
short of the largest system demand plus the outside hose times the duration 
requirement.  The city supply to the tank will be more than able to make up the 
difference.  The underwriter is saying that the “reliable automatic refill” 
cannot be considered.



I was wanting to show proof that it was acceptable prior to the 2013 edition.











From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Friday, January 27, 2017 3:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Tank Capacity



It was in one edition of 13R wayback when. I don't think it had ever been 
"allowed" by 22 until recently but it only makes sense. Now define reliable 
refill rate for this application emphasizing reliable.

On Fri, Jan 27, 2017 at 12:48 PM Brad Casterline <bcasterli...@gmail.com> wrote:

Requirements for break tanks were added NFPA 20 (2007), according to page 20-2.

Brad

On Jan 27, 2017 2:41 PM, "Mike B Morey" <mmo...@shambaugh.com> wrote:

The earliest reference I can find is NFPA 25 2007 in section 5.30, it has moved 
around since, but as others have pointed out, it's defined in there as a break 
tank.

  _


Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 <tel:(260)%20487-7824>  /  cell 260.417.0625 
<tel:(260)%20417-0625>  /  fax 260.487.7991 <tel:(260)%20487-7991>
email mmo...@shambaugh.com







From:Dale Wingard <da...@aaafp.com>
To:"sprinklerforum@lists.firesprinkler.org" 
<sprinklerforum@lists.firesprinkler.org>
Date:01/27/2017 02:52 PM
Subject:Tank Capacity
Sent by:"Sprinklerforum" 
<sprinklerforum-boun...@lists.firesprinkler.org>

  _




NFPA 22 (2013 Edition) excerpt-

4.1.4 A tank shall be sized so that the stored supply plus reliable automatic 
refill shall be sufficient to meet the demand placed upon it for the design 
duration.

I have researched earlier editions but I have not been able to find where the 
reliable automatic refill has been previously allowed; however, I recall this 
being the case.  Am I overlooking something?

Thanks,



 [attachment "Dale Wingard  SET.vcf" deleted by Mike B 
Morey/Shambaugh/EMCORGROUP] ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=GKdB6-XpYq_0W-WluyVHtw=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg=ZIlAYkYGG--WYErIebjpFDdfGghXLB-667jMo2EgODU=qOSLfkv2O4_vGbMHmTDjJ1Ouas46DTZW6qD5O1rpvcc=>
 
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=GKdB6-XpYq_0W-WluyVHtw=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg=ZIlAYkYGG--WYErIebjpFDdfGghXLB-667jMo2EgODU=qOSLfkv2O4_vGbMHmTDjJ1Ouas46DTZW6qD5O1rpvcc=

This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

--

Sent from Gmail Mobile



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: PIV Supervion, lock or tamper switch?

2017-01-23 Thread Art Tiroly
Local code determines when and where protection is required.

NFPA shows how it is to be done.

 

Art Tiroly

ATCO Fire Pro

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Owen Evans
Sent: Monday, January 23, 2017 12:26 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: PIV Supervion, lock or tamper switch?

 

As most of you know, I work exclusively with 13D systems. I do on occasion get 
questions on the big boy systems, 13 and 13R.  The property in question is a 
boutique hotel, two buildings. One building is a two story, fifty room hotel 
and the other building is two story, restaurant on the first floor and banquet 
facility on second floor with a roof deck. Each building has a FDC and a PIV. I 
am in California which is under the 2013 IFC. 

 

I recently had the question asked "does the PIV require electrical 
supervision?"  NFPA states a lock is adequate, the 2013 IFC states electrical 
supervision is required, with exceptions. I get different answers form 
different people. I'm thinking it's the more restrictive  2013 IFC. Which is it?

 

Thank you,

Owen Evans

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: College Lab Classrooms

2016-12-05 Thread Art Tiroly
A worst case would be quantity of flammable liquids.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net
Sent: Monday, December 05, 2016 11:39 AM
To: sprinklerforum
Subject: Re: College Lab Classrooms



Thank you everyone. Since this is a science lab I am going with OH2 to be safe.





  _

From: "Reed A. Roisum, SET" <raroi...@kfi-eng.com>
To: "sprinklerforum" <sprinklerforum@lists.firesprinkler.org>
Sent: Monday, December 5, 2016 11:07:56 AM
Subject: RE: College Lab Classrooms



Check out NFPA 45 Table 9.1.1(b).  This will give you a fire hazard class based 
on quantities of flammable and combustible liquids.  Then if you look in 
chapter 6 (6.1.1.1) it will tell you whether it is OH1 or OH2.



I know the MN Fire Code for instance says “Chemistry Labs” are OH2 but it makes 
sense to me that it would depend on the type and quantities of combustible 
liquids.



Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |  
<http://www.kfiengineers.com/> KFIengineers.com

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net
Sent: Monday, December 5, 2016 9:36 AM
To: sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: College Lab Classrooms



Quick question.

College Lab classrooms.  Light or Ordinary hazard?



Bill Menster
WFM Consulting Inc.
2416 Malaya Ct.
Punta Gorda, FL 33983
ph. 941-421-9786
fax 941-391-6133
wmens...@comcast.net
www.wfmconsultinginc.com <http://www.wfmconsultinginc.com/>




__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
<http://www.symanteccloud.com/>
__


__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sidewall Sprinkler in Peaked Skylight

2016-11-21 Thread Art Tiroly
What is RCMP?
Is the skylight less than 3 Ft high?
Is the volume less than 1000 Cu.Ft.?
If yes to both no sprinklers are required in the skylight.

Art Tiroly
ATCO Fire/Tiroly


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of P & P Sprinklers Ltd
Sent: Monday, November 21, 2016 6:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sidewall Sprinkler in Peaked Skylight

We are sprinklering 2 new RCMP buildings, both having the same design and
layout. The roof has a 12/12 pitch and has a skylight running along the
ridge 27 ft in length and 5 ft wide. How would one go about properly
protecting this skylight? It seems by code it isn't allowed to put a
sidewall in the peak at both ends, though that is exactly what is shown in
the engineers plans. Has anyone come across this situation?

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR retrofit

2016-11-09 Thread Art Tiroly
Measure the ID of the brass nipple.

The ID is near 1”.

Can you get a 1x3/4 male reducer. Think about velocity and turbulence at  ~ 125 
gpm



Art



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Wednesday, November 09, 2016 4:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR retrofit



I am looking at a warehouse space that needs to upgrade from K14 ESFR to K22. 
Typically this would involve plugging the ¾” outlets and cutting in new 1” 
mechanical T’s.



I had someone ask why we could not use a ¾” brass nipple and a ¾” to 1” reducer 
to  up-size the outlet to hold a 1” head. I feel like this is not allowed, but 
I could not find specifically where. It would not really be an extension 
fitting. ¾” brass is allowed. Each change of size is done with a single piece 
reducer. The ¾” tee and nipple would be included in the calculations…



Any help on where the code addresses this setup?



Thanks!



Matt Grisé PE*, LEED AP, NICET II
Vice President – New Construction
Alliance Fire Protection

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO



913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com







---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprikler obstruction.

2016-10-20 Thread Art Tiroly
Thank you.

Does the same effect occur next to a duct we wonder.

The ceiling area forms a pocket that is 4’ from an adjacent wall 4Ft away to 
sprinkler that is next to a duct.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, October 20, 2016 4:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



>From the 1984 Technical Committee Reports for Proposal 13-401:



“SUBSTANTIATION Guidance is needed for the placement of standard sprinklers (ie 
non sidewall heads) in relation to their horizontal proximity to walls. Dead 
air spaces in corners can effect a sprinkler’s operation time. The minimum 
clearance for sidewall was used (NFPA 13  4-5.4). A recent installation in a 
300 ft long by 9 ft wide corridor caused this concern when the sprinklers were 
located only 1 in off the wall.”



Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: October-20-16 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What is the reasoning for the 4” minimum space to a wall or duct?

It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.



Art at ATCO Fire







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprikler obstruction.



For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.



On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What size is the duct and what is the distance between the sprinkler and the 
top of duct.





De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: Re: Sprikler obstruction.



Is the duct below the sprinkler deflector?





On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





  _


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 Imagen quitada por el remitente. Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





  _


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 Image removed by sender. Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







--

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprikler obstruction.

2016-10-20 Thread Art Tiroly
The 12”duct is not a wall.

Then sidewall sprinklers would not function properly either.

An old timers reason was how to install a screwed tee with two wrenches less 
than 4” from an object.

This sprinkler was there before the duct.



This question comes from a fire prevention officer.

Art at ATCO





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Thursday, October 20, 2016 1:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprikler obstruction.



Doesn't it have something with the heat plume and how it "bends" at the wall / 
ceiling interface.



Heat detectors can't be within four inches of a wall either, if I recall 
correctly. And that make sense as a sprinkler is a form of heat detector any 
way.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Oct 20, 2016, at 9:36 AM, rongreenman . <rongreen...@gmail.com> wrote:

I was told it has to do with pattern development, splash back from the wall 
interference. This is sitting in my bucket of potential to probably old 
fitters' (wives') tales until I get confirmation from more 
reliable/knowledgeable sources than the guy that told me this.



On Thu, Oct 20, 2016 at 6:41 AM, Art Tiroly <atir...@atcofirepro.com> wrote:

What is the reasoning for the 4” minimum space to a wall or duct?

It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.



Art at ATCO Fire







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprikler obstruction.



For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.



On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What size is the duct and what is the distance between the sprinkler and the 
top of duct.





De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: Re: Sprikler obstruction.



Is the duct below the sprinkler deflector?





On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





  _


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





  _


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







--

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com

253.576.9700



The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)


___
Sprinklerforum mai

RE: Sprikler obstruction.

2016-10-20 Thread Art Tiroly
What is the reasoning for the 4” minimum space to a wall or duct?

It isn’t activation or spray pattern since sidewall sprinklers operate in a 
recessed escutcheon.

 

Art at ATCO Fire

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Wednesday, October 19, 2016 5:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprikler obstruction.

 

For standard spray sprinklers: 4" from the duct unless a sidewall (you could 
use a vertical type) and no closer the 6' from the next closest sprinkler. The 
rules are pretty clear. Unless you can find a sprinkler who's listing negates 
these rules you're stuck.

 

On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <atir...@atcofirepro.com 
<mailto:atir...@atcofirepro.com> > wrote:

12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.

 

Art

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> ] On Behalf Of Cesar 
Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Sprikler obstruction.

 

What size is the duct and what is the distance between the sprinkler and the 
top of duct.

 

 

De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Asunto: Re: Sprikler obstruction.

 

Is the duct below the sprinkler deflector?

 

 

On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <atir...@atcofirepro.com 
<mailto:atir...@atcofirepro.com> > wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899  

216-570-7030   cell

 

 

  _  


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
  

 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

 

  _  


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
  

 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





 

-- 

Ron Greenman


4110 Olson Dr., NW
Gig Harbor, WA 98335

rongreen...@gmail.com <mailto:rongreen...@gmail.com> 

253.576.9700

 

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprikler obstruction.

2016-10-19 Thread Art Tiroly
12x16” Duct is tight to ceiling.

Up right Sprinkler is about 6” from ceiling on exposed pipe.

Fire Marshall’s issue is that the sprinkler is about 2.5” from the face of the 
duct.

Adjacent sprinkler is about 6’-0 away.



Art



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 19, 2016 4:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.



What size is the duct and what is the distance between the sprinkler and the 
top of duct.





De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: Re: Sprikler obstruction.



Is the duct below the sprinkler deflector?





On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

Does an upright sprinkler have to be moved when a new duct was added less than 
4” away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4” away from a wall.

I have adequate coverage from the adjacent sprinkler in this basement meeting 
room space.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





  _


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>
 Imagen quitada por el remitente. Avast logo

This email has been checked for viruses by Avast antivirus software.
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient>




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sprikler obstruction.

2016-10-19 Thread Art Tiroly
Does an upright sprinkler have to be moved when a new duct was added less
than 4" away from the existing  sprinkler.

I understand when a new sprinkler is installed it shall be 4" away from a
wall.

I have adequate coverage from the adjacent sprinkler in this basement
meeting room space.

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FM Global

2016-09-29 Thread Art Tiroly
You will also have to meet local code requirements per NFPA 13 for submittal 
whichever is geater.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Thursday, September 29, 2016 10:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FM Global



Thanks guys, I didn’t even know about 3-26.  We will confirm everything with FM 
before submitting.



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Thursday, September 29, 2016 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FM Global



When I have done “non-factory” projects with FM global (most recently a 
retirement home) they were very flexible in modifying their requirements to 
suit the project. In occupancies that don’t directly correlate to their core 
business I have had good luck with compromises.



Cesar is right  – confirm all design guidelines in writing from FM if they are 
any different from the ones spelled out in the data sheets.



Matt Grisé PE*, LEED AP, NICET II
Vice President – New Construction
Alliance Fire Protection

130 w 9th Ave.
North Kansas City, MO 64116


*Licensed in KS & MO



913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Thursday, September 29, 2016 9:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: FM Global



Hi Dewayne.



Accord to 3-26 table 1. Both areas Seating areas and kitchen are a HC1 Hazard 
and sprinkler design is 0.1/1500 + 250 gpm using a 5.6 k factor sprinklers.

Also you need to wait for FM insurance recommendations.



CLR



De: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] En 
nombre de Dewayne Martinez
Enviado el: jueves, 29 de septiembre de 2016 08:14 a. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: FM Global



We are doing a small restaurant tenant in a strip mall that is insured by FM 
Global.  I have contacted the GC asking for the FM contact but thought maybe 
the forum could provide some insight.  1)Does FM allow reduced design areas? 
2)Seating area 01./1500 +100gpm and kitchen 0.15/1500 +250gpm sound right?

Thanks,

Dewayne



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Open-Grid Ceilings - Egg crate

2016-09-15 Thread Art Tiroly
Sprinklers above the egg crate will have obstructed flow spray pattern.

How far below the deck are the sprinklers in the egg crate ceiling?

If more than 12"???

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of J.P. Merlino/Ing. L.Lagomarsino & Asoc.
Sent: Thursday, September 15, 2016 6:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Open-Grid Ceilings - Egg crate

 

Dear Sirs:

NFPA 13 Ed. 2016 - 8.15.14

If we have an open grid egg-crate that meets 70% open space but the depth of
the material (2 in) exceeds the least dimension (1 in) it does not comply
with the allowance not to install sprinkler beneath and we must install in
the egg-crate (or beneath).

But the standard is silent on what to do with the space over the egg-crate.
Shall we have two layers of sprinklers, one in the egg-crate and the other
over the egg-crate as if the egg-crate does not exist?

I appreciate your thoughts or if we are missing something.

best regards

J.P. Merlino



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ceiling Pockets

2016-09-13 Thread Art Tiroly
Thank you. Some of the window pockets are 30-50 Ft. long but still under
1000 Cu.Ft..

Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be
the prime consideration not a 4Ft high pocket along an outside window wall.

 

When you divide 1000 by 3 = 333.3 SF. That is a big area with no sprinklers.

Depends on the shape of the pocket.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday, September 13, 2016 1:36 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets

 

That makes sense, until you start taking it to extremes.  What about a 10'
deep pocket under 1000 sq ft?  I guess the committee had to draw a line
somewhere and 3' was the line.  Even though it is potentially a bunch of
extra sprinklers, the smaller orifices should limit the hydraulic impact.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com
 
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

On 9/13/2016 10:29 AM, Art Tiroly wrote:

Thank you. Some of the window pockets are 30-50 Ft. long but still under
1000 Cu.Ft..

Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be
the prime consideration not a 4Ft high pocket along an outside window wall.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of T. Silva
Sent: Tuesday, September 13, 2016 12:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets

 

Skylights and similar pockets not exceeding 32 sq.ft. and separated from
other pockets by minimum 10 feet do not require sprinklers. I would try to
use that.

Tony


  _  


From: "Travis Mack" <tm...@mfpdesign.com>
To: sprinklerforum@lists.firesprinkler.org
Sent: Tuesday, September 13, 2016 9:34:20 AM
Subject: Re: Ceiling Pockets

Just put a 2.8k sprinkler in the pocket. At least that minimizes the
hydraulic impact to the system. 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Sep 13, 2016, at 8:21 AM, Art Tiroly <atir...@atcofirepro.com> wrote:

I have 4 Ft wide x 4 Ft deep window pockets in a 100 year old class room
building with new drop ceilings.  Adding a sprinkler to a window pocket
because it is over 3 Ft. deep makes no sense to me in these class rooms.
If a pocket sprinkler activates and washes the windows it does nothing for
the fire 8-12 Ft. away. I plan to ask for a variance from the Ohio State
plans examiner at submittal though likely to no avail.

 

Art Tiroly

ATCO Fire Protection

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: Monday, September 12, 2016 5:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets

 

It's all about activation Ron/Bruce.
Roland's insight as to the pass/fail criteria was a stroke of genius.

I like to explain it and then Roland corrects me. So I'll forego my part and
wait for Roland to get his ears on.

Brad

On Sep 12, 2016 4:41 PM, "Bruce Verhei" <bver...@comcast.net> wrote:

Ron is briefer.


On Sep 12, 2016, at 14:39, Bruce Verhei <bver...@comcast.net> wrote:

Isn't the idea of using a Volume completely different than viewing his as an
Area, such as a large sail sewing table that obstructs coverage as well as
delaying operation?

 

Wasn't 1,000 cu ft a consensus guesstimate saying we'd allow a space this
big for heat to accumulate in before banking down to activate heads? And
experience presumably has shown it works, usually?

 

Putting a head to cover part of it is better if fire is under that head. If
fire is away from head will you delay heat from banking down, resulting in a
worse situation? I don't know. And I would guesstimate original designer
doesn't either.

 

Best

 

Bruce Verhei


On Sep 12, 2016, at 11:21, T. Silva <silva...@shaw.ca> wrote:


  _  


NFPA 13, 2013

8.6.7.2 (1) "The total volume of the unprotected ceiling pocket does not
exceed 1000 cu.ft."

Is the 1000 cuft only the volume of the pocket that is not sprinklered? For
example, there is a pocket that is 30" long x 20' wide x 2' deep, creating a
1200 cuft ceiling pocket. If one row of sprinklers are provided in this
pocket (along the 30 foot length), to provi

RE: Ceiling Pockets

2016-09-13 Thread Art Tiroly
Thank you. Some of the window pockets are 30-50 Ft. long but still under 1000 
Cu.Ft..

Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be the 
prime consideration not a 4Ft high pocket along an outside window wall.



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Tuesday, September 13, 2016 1:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets



If I wer interpreting I'd be thinking pockets at the roof that are not 
skylights are what are similar to skylights, not pockets in walls. Fortunately 
for you I'm not the one you need to convince. Essentially you have a broken 
soffit with a raised floor (presuming the windows aren't at the regular floor 
level.

On Tuesday, September 13, 2016, T. Silva <silva...@shaw.ca> wrote:

Skylights and similar pockets not exceeding 32 sq.ft. and separated from other 
pockets by minimum 10 feet do not require sprinklers. I would try to use that.

Tony

  _

From: "Travis Mack" <tm...@mfpdesign.com 
<javascript:_e(%7B%7D,'cvml','tm...@mfpdesign.com');> >
To: sprinklerforum@lists.firesprinkler.org 
<javascript:_e(%7B%7D,'cvml','sprinklerforum@lists.firesprinkler.org');>
Sent: Tuesday, September 13, 2016 9:34:20 AM
Subject: Re: Ceiling Pockets

Just put a 2.8k sprinkler in the pocket. At least that minimizes the hydraulic 
impact to the system.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Sep 13, 2016, at 8:21 AM, Art Tiroly <atir...@atcofirepro.com 
<javascript:_e(%7B%7D,'cvml','atir...@atcofirepro.com');> > wrote:

I have 4 Ft wide x 4 Ft deep window pockets in a 100 year old class room 
building with new drop ceilings.  Adding a sprinkler to a window pocket because 
it is over 3 Ft. deep makes no sense to me in these class rooms.   If a pocket 
sprinkler activates and washes the windows it does nothing for the fire 8-12 
Ft. away. I plan to ask for a variance from the Ohio State plans examiner at 
submittal though likely to no avail.



Art Tiroly

ATCO Fire Protection





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<javascript:_e(%7B%7D,'cvml','sprinklerforum-boun...@lists.firesprinkler.org');>
 ] On Behalf Of Brad Casterline
Sent: Monday, September 12, 2016 5:51 PM
To: sprinklerforum@lists.firesprinkler.org 
<javascript:_e(%7B%7D,'cvml','sprinklerforum@lists.firesprinkler.org');>
Subject: Re: Ceiling Pockets



It's all about activation Ron/Bruce.
Roland's insight as to the pass/fail criteria was a stroke of genius.

I like to explain it and then Roland corrects me. So I'll forego my part and 
wait for Roland to get his ears on.

Brad

On Sep 12, 2016 4:41 PM, "Bruce Verhei" <bver...@comcast.net 
<javascript:_e(%7B%7D,'cvml','bver...@comcast.net');> > wrote:

Ron is briefer.


On Sep 12, 2016, at 14:39, Bruce Verhei <bver...@comcast.net 
<javascript:_e(%7B%7D,'cvml','bver...@comcast.net');> > wrote:

Isn't the idea of using a Volume completely different than viewing his as an 
Area, such as a large sail sewing table that obstructs coverage as well as 
delaying operation?



Wasn't 1,000 cu ft a consensus guesstimate saying we'd allow a space this big 
for heat to accumulate in before banking down to activate heads? And experience 
presumably has shown it works, usually?



Putting a head to cover part of it is better if fire is under that head. If 
fire is away from head will you delay heat from banking down, resulting in a 
worse situation? I don't know. And I would guesstimate original designer 
doesn't either.



Best



Bruce Verhei


On Sep 12, 2016, at 11:21, T. Silva <silva...@shaw.ca 
<javascript:_e(%7B%7D,'cvml','silva...@shaw.ca');> > wrote:


  _


NFPA 13, 2013

8.6.7.2 (1) "The total volume of the unprotected ceiling pocket does not exceed 
1000 cu.ft."

Is the 1000 cuft only the volume of the pocket that is not sprinklered? For 
example, there is a pocket that is 30" long x 20' wide x 2' deep, creating a 
1200 cuft ceiling pocket. If one row of sprinklers are provided in this pocket 
(along the 30 foot length), to provide a protected area of 30' x 10'

(1) Is the the total volume of the unprotected ceiling pocket still 1200 cuft? 
or
(2) Reduced to 600 cuft, discounting the sprinklered area?

Thanks,

Tony

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<javascript:_e(%7B%7D,'cvml','Sprinklerforum@lists.firesprinkler.org');>
http://lists.

RE: Ceiling Pockets

2016-09-13 Thread Art Tiroly
Thank you. Some of the window pockets are 30-50 Ft. long but still under 1000 
Cu.Ft..

Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be the 
prime consideration not a 4Ft high pocket along an outside window wall.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of T. Silva
Sent: Tuesday, September 13, 2016 12:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets



Skylights and similar pockets not exceeding 32 sq.ft. and separated from other 
pockets by minimum 10 feet do not require sprinklers. I would try to use that.

Tony

  _

From: "Travis Mack" <tm...@mfpdesign.com>
To: sprinklerforum@lists.firesprinkler.org
Sent: Tuesday, September 13, 2016 9:34:20 AM
Subject: Re: Ceiling Pockets

Just put a 2.8k sprinkler in the pocket. At least that minimizes the hydraulic 
impact to the system.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign



Sent from my iPhone


On Sep 13, 2016, at 8:21 AM, Art Tiroly <atir...@atcofirepro.com> wrote:

I have 4 Ft wide x 4 Ft deep window pockets in a 100 year old class room 
building with new drop ceilings.  Adding a sprinkler to a window pocket because 
it is over 3 Ft. deep makes no sense to me in these class rooms.   If a pocket 
sprinkler activates and washes the windows it does nothing for the fire 8-12 
Ft. away. I plan to ask for a variance from the Ohio State plans examiner at 
submittal though likely to no avail.



Art Tiroly

ATCO Fire Protection





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Monday, September 12, 2016 5:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets



It's all about activation Ron/Bruce.
Roland's insight as to the pass/fail criteria was a stroke of genius.

I like to explain it and then Roland corrects me. So I'll forego my part and 
wait for Roland to get his ears on.

Brad

On Sep 12, 2016 4:41 PM, "Bruce Verhei" <bver...@comcast.net> wrote:

Ron is briefer.


On Sep 12, 2016, at 14:39, Bruce Verhei <bver...@comcast.net> wrote:

Isn't the idea of using a Volume completely different than viewing his as an 
Area, such as a large sail sewing table that obstructs coverage as well as 
delaying operation?



Wasn't 1,000 cu ft a consensus guesstimate saying we'd allow a space this big 
for heat to accumulate in before banking down to activate heads? And experience 
presumably has shown it works, usually?



Putting a head to cover part of it is better if fire is under that head. If 
fire is away from head will you delay heat from banking down, resulting in a 
worse situation? I don't know. And I would guesstimate original designer 
doesn't either.



Best



Bruce Verhei


On Sep 12, 2016, at 11:21, T. Silva <silva...@shaw.ca> wrote:


  _


NFPA 13, 2013

8.6.7.2 (1) "The total volume of the unprotected ceiling pocket does not exceed 
1000 cu.ft."

Is the 1000 cuft only the volume of the pocket that is not sprinklered? For 
example, there is a pocket that is 30" long x 20' wide x 2' deep, creating a 
1200 cuft ceiling pocket. If one row of sprinklers are provided in this pocket 
(along the 30 foot length), to provide a protected area of 30' x 10'

(1) Is the the total volume of the unprotected ceiling pocket still 1200 cuft? 
or
(2) Reduced to 600 cuft, discounting the sprinklered area?

Thanks,

Tony

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ceiling Pockets

2016-09-13 Thread Art Tiroly
I have 4 Ft wide x 4 Ft deep window pockets in a 100 year old class room 
building with new drop ceilings.  Adding a sprinkler to a window pocket because 
it is over 3 Ft. deep makes no sense to me in these class rooms.   If a pocket 
sprinkler activates and washes the windows it does nothing for the fire 8-12 
Ft. away. I plan to ask for a variance from the Ohio State plans examiner at 
submittal though likely to no avail.

 

Art Tiroly

ATCO Fire Protection

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Monday, September 12, 2016 5:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Ceiling Pockets

 

It's all about activation Ron/Bruce.
Roland's insight as to the pass/fail criteria was a stroke of genius.

I like to explain it and then Roland corrects me. So I'll forego my part and 
wait for Roland to get his ears on.

Brad

On Sep 12, 2016 4:41 PM, "Bruce Verhei" <bver...@comcast.net 
<mailto:bver...@comcast.net> > wrote:

Ron is briefer.


On Sep 12, 2016, at 14:39, Bruce Verhei <bver...@comcast.net 
<mailto:bver...@comcast.net> > wrote:

Isn't the idea of using a Volume completely different than viewing his as an 
Area, such as a large sail sewing table that obstructs coverage as well as 
delaying operation?

 

Wasn't 1,000 cu ft a consensus guesstimate saying we'd allow a space this big 
for heat to accumulate in before banking down to activate heads? And experience 
presumably has shown it works, usually?

 

Putting a head to cover part of it is better if fire is under that head. If 
fire is away from head will you delay heat from banking down, resulting in a 
worse situation? I don't know. And I would guesstimate original designer 
doesn't either.

 

Best

 

Bruce Verhei


On Sep 12, 2016, at 11:21, T. Silva <silva...@shaw.ca <mailto:silva...@shaw.ca> 
> wrote:


  _  


NFPA 13, 2013

8.6.7.2 (1) "The total volume of the unprotected ceiling pocket does not exceed 
1000 cu.ft."

Is the 1000 cuft only the volume of the pocket that is not sprinklered? For 
example, there is a pocket that is 30" long x 20' wide x 2' deep, creating a 
1200 cuft ceiling pocket. If one row of sprinklers are provided in this pocket 
(along the 30 foot length), to provide a protected area of 30' x 10'  

(1) Is the the total volume of the unprotected ceiling pocket still 1200 cuft? 
or
(2) Reduced to 600 cuft, discounting the sprinklered area?

Thanks,

Tony

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ceiling pockets

2016-08-04 Thread Art Tiroly
He intent is to use either 8.7.7 or 8.8.7 for large pockets.

The volume of the pocket seems more important than the depth.

A 4x4x40-50'  pocket should not need sprinklers next to glass windows.

 

 

Art Tiroly

ATCO Fire Protection

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Ed Kramer
Sent: Thursday, August 04, 2016 3:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Ceiling pockets 

 

If you qualify, you might be able to use 8.8.7.3.  Note the wording ". . and
similar pockets."  Section 8.5.7 doesn't limit the depth to 3'. 

 

Ed Kramer

Bamford Fire

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Thursday, August 04, 2016 11:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Ceiling pockets 

 

In section 8.8.7 sprinklers may be omitted from 1000 Cu.Ft. ceiling pockets.

This large volume is allowed but is further restricted by a 3 Ft. maximum
pocket height.

I have long narrow pockets along high windows with a new drop ceiling that
has a pocket 4 Ft. above the new ceiling.

The volumes are less than 1000 Cu.Ft.

I don't understand the restriction to 3 Ft. since the air volume seems to be
the relevant restriction.

Do I need to add sprinklers to a ceiling pocket along the windows when I
have floor coverage.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=icon> Image removed by sender.

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=link> www.avast.com 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Ceiling pockets

2016-08-04 Thread Art Tiroly
In section 8.8.7 sprinklers may be omitted from 1000 Cu.Ft. ceiling pockets.

This large volume is allowed but is further restricted by a 3 Ft. maximum
pocket height.

I have long narrow pockets along high windows with a new drop ceiling that
has a pocket 4 Ft. above the new ceiling.

The volumes are less than 1000 Cu.Ft.

I don't understand the restriction to 3 Ft. since the air volume seems to be
the relevant restriction.

Do I need to add sprinklers to a ceiling pocket along the windows when I
have floor coverage.

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: acid corosion

2016-07-13 Thread Art Tiroly
Sorry for the repetition. I did not think this was getting through.

 

Art

 

[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Wednesday, July 13, 2016 3:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 

 

 

 

We have an issue with sprinkler water becoming acidic 5.5-6 PH.

System is 6 months old. The Bellville seal corrodes and cracks resulting in
drips from sprinkler.

6 sprinklers so far. Columbus water is not acidic. Test from back flow drain
shows acid 5.6 PH

Manufacturer says it is acid water corrosion that damages seal.

 

Other tests also acidic. Goes acidic in two weeks. Foul smelling with
particulates.

Some black pipe, mostly CPVC in an old Frat house

System drained and filled 6 times.

What can be causing low PH in a few weeks.

Pictures show corrosion inside the sprinkler throat and seal.

There is also an glycerin antifreeze system that does not have this problem.

 

Suggestions please

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


 
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=oa-2368-c> Image removed by
sender.

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email_source=link_campai
gn=sig-email_content=emailclient_term=oa-2368-c> www.avast.com 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE:

2016-07-13 Thread Art Tiroly
 

 

We have an issue with sprinkler water becoming acidic 5.5-6 PH.

System is 6 months old. The Bellville seal corrodes and cracks resulting in
drips from sprinkler.

6 sprinklers so far. Columbus water is not acidic. Test from back flow drain
shows acid 5.6 PH

Manufacturer says it is acid water corrosion that damages seal.

 

Other tests also acidic. Goes acidic in two weeks. Foul smelling with
particulates.

Some black pipe, mostly CPVC in an old Frat house

System drained and filled 6 times.

What can be causing low PH in a few weeks.

Pictures show corrosion inside the sprinkler throat and seal.

There is also an glycerin antifreeze system that does not have this problem.

 

Suggestions please

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


FW: Leaking sprinkler due to corrosion

2016-07-13 Thread Art Tiroly




From: Art Tiroly [mailto:atir...@atcofirepro.com]
Sent: Wednesday, July 13, 2016 2:07 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: Leaking sprinkler due to corrosion





We have an issue with sprinkler water becoming acidic 5.5-6 PH.

System is 6 months old. The Bellville seal corrodes and cracks resulting in 
drips from sprinkler.

6 sprinklers so far. Columbus water is not acidic. Test from back flow drain 
shows acid 5.6 PH

Manufacturer says it is acid water corrosion that damages seal.



Other tests also acidic.

Some black pipe, mostly CPVC in an old Frat house

System drained and filled 6 times.

What can be causing low PH in a few weeks.

Pictures show corrosion inside the sprinkler throat and seal.

There is also an antifreeze system that does not have this problem.



Suggestions please



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Leaking sprinkler due to corrosion

2016-07-13 Thread Art Tiroly


We have an issue with sprinkler water becoming acidic 5.5-6 PH.

System is 6 months old. The Bellville seal corrodes and cracks resulting in 
drips from sprinkler.

6 sprinklers so far. Columbus water is not acidic. Test from back flow drain 
shows acid 5.6 PH

Manufacturer says it is acid water corrosion that damages seal.



Other tests also acidic.

Some black pipe, mostly CPVC in an old Frat house

System drained and filled 6 times.

What can be causing low PH in a few weeks.

Pictures show corrosion inside the sprinkler throat and seal.

There is also an antifreeze system that does not have this problem.



Suggestions please



Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Acidic Corrosion

2016-07-13 Thread Art Tiroly
We have an issue with sprinkler water becoming acidic 5.5-6 PH.

System is 6 months old. The Bellville seal corrodes and cracks resulting in
drips from sprinkler.

6 sprinklers so far. City water is not acidic. Test from back flow drain
shows acid 5.6.

Manufacturer says it is acid water corrosion.

 

Other tests also acidic.

Some black pipe, mostly CPVC in an old Frat house

System drained and filled 6 times.

What can be causing low PH in a few weeks.

Pictures show corrosion inside the sprinkler throat and seal.

There is also an antifreeze system that does not have this problem.

 

Suggestions please

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Calculating extended coverage

2016-07-13 Thread Art Tiroly
What state are you in?

Can I assume you are planning quick response sprinklers. 

Then why not 900 SF area of application allowance?

What part of the code is AHJ using for this requirement.

There are residential rules in 13.

Use residential heads with .10 density

 

Art Tiroly

Tiroly and Associates

 

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jay Stough
Sent: Wednesday, July 13, 2016 10:51 AM
To: Sprinkler Forum <sprinklerforum@lists.firesprinkler.org>
Subject: Calculating extended coverage

 

I have a nursing care facility that I am trying to calc.  Must be 13 (2007) 
light.  Can not use room design or residential method per state AHJ.  The 
building is shaped like an upper case H with the bottom legs cut off.  There 
are 4 rooms on one side of the corridor and 3 rooms on the other side of the 
corridor in each upper leg that use extended coverage sprinkler in each room.  
Also 1 standard spray sprinkler in a closet and one standard spray sprinkler in 
a bathroom in each room.  Sprinklers in the corridor are standard spray also.  
Since I am using extended coverage sprinklers, I need to calculate 5 minimum.  
The sprinklers cover 16'3 X 14', so need to calc at the 18' X 18' rate.  
22.4.6.2 allows me in "rooms like closets, washrooms and similar small 
compartments requiring only one sprinkler shall be permitted to be omitted from 
calculations within the area of application".   Can I calculate 6 extended 
coverage sprinklers, without the corridor or "small rooms or compartments" for 
my 1500 sq ft?  Or should I calc 5 extended coverage and the hallway sprinklers 
in the 1500 sq ft?  



Jay Stough 

NICET IV LAYOUT 

NICET III ITM

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Two Backflows

2016-06-23 Thread Art Tiroly
Water company requires BFP not NFPA 13, 24.

 

Art Tiroly

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Thursday, June 23, 2016 11:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Two Backflows

 

I use RPZ as a generic term.

 

Also I am going under the assumption that I MUST separate my sprinkler from
the domestic at the point of connection. However it was brought to my
attention that this may not be required in NFPA anyway. While the thought of
sprinkler water and domestic water sickens me a bit . can someone show me
where NFPA says I must separate them with a backflow?

 

John Irwin

Sprinkler Construction Manager 

Critical System Solutions, LLC
Cell: 813.618.2781

Email:  jir...@criticalsystemsolutions.com
<mailto:jir...@criticalsystemsolutions.com> 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Thursday, June 23, 2016 11:07 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Two Backflows

 

I don't think there's any prohibition and we've been asked to do this
before.  I would check with serving water and fire departments to be sure
that both devices satisfy the requirement of their respective masters.
RPZ's are not UL classified for fire service and usually configured with
non-indicating valves for general water service.   NFPA standards require
ALL valves controlling fire protection water supplies to be LISTED (for fire
service) indicating type and building code requires them to be supervised.
Have fun .

 

Steve

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Thursday, June 23, 2016 8:03 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Two Backflows

 

I am working on a project where the developer and site contractor have
decided that fire and domestic should share an underground line around the
site and to the building. At the street there is a meter assembly and a
Wilkins 375A RPZ. I would need to install an additional backflow at my point
of connection because the line is shared all the way to the water room.
Other than being a dumb way to do this and having two pressure losses in my
calculations, is there any code that says I can't gave two RPZs in my water
line?

 

 

John Irwin

Sprinkler Construction Manager

 

Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL  33716
Office: 727.209.5122

Fax:  727.209.5126

Cell: 813.618.2781

Email:  jir...@criticalsystemsolutions.com
<mailto:jir...@criticalsystemsolutions.com> 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Forward Flow for a Backflow Preventer

2016-04-26 Thread Art Tiroly
Easy. Calculate GPM through the 1" pipe and fittings in drain line. Doubt you 
will 100 gpm.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Tuesday, April 26, 2016 2:46 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Forward Flow for a Backflow Preventer

I did an article in Sprinkler Age (2013 but not sure which issue) on ow to 
calculate it as well as other options for the forward flow test.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Apr 26, 2016, at 10:15 AM, James Crawford <jcrawf...@phaserfire.ca> wrote:
> 
> I know this has been discussed but can’t seem to find it.
> 
> 
> 
> NFPA #13 (2013) 8.17.4.6.1 Means shall be provided downstream of all 
> backflow prevention valves for flow tests at system demand.
> 
> 
> 
> We have a small office system, system demand 160 gpm, we have 100 psi 
> static pressure, the system has a 2 ˝” riser so a 1 Ľ” drain, how much 
> water can we get out of an 1 Ľ” drain?
> 
> 
> 
> Is there anything out there to help determine the size and or number 
> of outlets required to forward flow at different system demands?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  jcrawf...@phaserfire.ca
> 
> 
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Class IIIB Liquid Storage

2016-03-30 Thread Art Tiroly
Design requirements are in NFPA 30.
How high is storage?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent: Wednesday, March 30, 2016 1:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Class IIIB Liquid Storage

A client has a building that is protected with an Ordinary Hazard Group 3
system.

 

They want to store class IIIB combustible liquids in 16 gal and 55 gal
drums.

 

Table 9.6.1 gives the MAQ for a IIIB as 13,200 gal with note 1 & 4 and note
4 states that the quantities are not limited if the building is equipped
with an automatic sprinkler system installed in accordance with NFPA #13.
This seems to imply that they could store an unlimited amount of class IIIB
liquids.

 

Table 12.6.2.2 gives the MAQ as 55,000 gal if the building is protected with
a sprinkler system designed for class 4 commodities to 20'.

 

Am I missing something

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: EC sprinkler identification

2016-03-23 Thread Art Tiroly
Sometimes you have to wake me up. I just saw this question.

Went to google. Tyco uses EC #'s. I saw EC 5, 8, 11, 14 but no EC 10 in
there listing.

Call Tyco they can help. What size is pipe thread. 1/2 or 3/4"?

Art

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Dewayne Martinez
Sent: Thursday, January 21, 2016 3:01 PM
To: SprinklerFORUM
Subject: EC sprinkler identification

Extended coverage link horizontal sidewall with EC-10 on the deflector.
Any clue on the mfg?

Thanks,

Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Old pipe schedule

2016-03-19 Thread Art Tiroly
What is the sprinkler spacing?
Staggered spacing was quite common before 1940.
Newer heads installed?
High pressure water supply connected?
It likely will barely do .10 density or maybe .15 with moderate pressure.
FM used to allow 3-5 psi at end head for pipe schedule.

Art Tiroly
ATCO Fire Protection

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Wednesday, March 16, 2016 7:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Old pipe schedule

I am working on a project in a mill that was constructed in 1884. On the top
floor, the branch piping is 3/4 - 1 - 1. Was there an older version of pipe
schedule that allowed smaller pipe or is this just undersized? 
Hopefully some of you history buffs (or at least those with a bunch of old
stuff) would know.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinkler Distance from insulated ceilings

2016-03-02 Thread Art Tiroly
Sprinklers don't spray upward. If Foam plastic insul is combustible it burns
faster 
than the sprinklers can operate and water is not sprayed upward.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Richard Carr
Sent: Wednesday, March 02, 2016 12:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler Distance from insulated ceilings 

1"-12" below insulation.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com
904-781-8227

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Thomas Reinhardt
Sent: Wednesday, March 02, 2016 11:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sprinkler Distance from insulated ceilings 

Can someone explain to me(sorry I just can't seem to visualize what they are
saying. I have a company that wants to spray insulation up on the metal deck
of the warehouse. The building is currently sprinklered with branch lines
and uprights. I have looked at NFPA 13  2010 sections 8.5.4.1.3.1 and
8.5.4.1.3.2. How far must the deflector be from the sprayed insulation. Just
for note I have researched the flame spread and smoke index of the
insulation. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
thomas.reinha...@skokie.org<mailto:thomas.reinha...@skokie.org>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Oversized fire pump

2016-02-16 Thread Art Tiroly
In Ohio we are required to provide a low suction control panel that will
shut the pump off and sound an alarm.
Later we now must provide a pressure sustaining valve that throttles the
fire pump discharge flow to maintain a predetermined low suction pressure 10
psi on the suction to protect the public water pressure


Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 11:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Oversized fire pump

Mark,
The 18 psi suction pressure is at the suction flange of the pump. There is
friction loss in the underground piping and BFP so the pressure at the
street will be greater. Given we have a steep curve (90 static and goes to 0
at
1900
gpm) and the size of the pump (1500 at 85), I am concerned if we have a big
draw in an uncontrolled situation, unlike a pump test, do we have the
potential of a serious problem.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Tue, Feb 16, 2016 at 11:13 AM, mphe...@aerofire.com
<mphe...@aerofire.com>
wrote:
Todd,
When you talk about drawing the suction pressure down to 20 psi, is your
reference point at the pump suction gauge, or at the connection to the city
water main?
Mark at Aero
602 820-7894

-Original Message-
 From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd
Williams
Sent: Tuesday, February 16, 2016 8:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Oversized fire pump

No the water supply was the same. Not sure where this came from but could be
an IOR mistake.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
On Tue, Feb 16, 2016 at 10:46 AM, craig.pr...@ch2m.com
<craig.pr...@ch2m.com>
wrote:
It may have been sized correctly in 2009 but the municipal water supply has
degraded since then.

Suction control valve is the way to go to fix the problem. That will keep
the supply from being drawn down below 20 psi.

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com



-Original Message-
 From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd
Williams
Sent: Tuesday, February 16, 2016 7:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Oversized fire pump

I am working on a facility with a fire pump that was oversized for the
available public water supply. The pump is 1500 gpm at 85 psi. At 1500 gpm,
the suction pressure drops to 18 psi. This is characteristic of the water
supply and is not due to a shut valve or other obstruction. The pump was
installed in 2009.
Are
there any safeguards that I should recommend for this situation?

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



RE: Galvanized in 1986 wet system

2016-02-01 Thread Art Tiroly
Some threadable light wall pipe was galvanized on the outer pipe wall but
not inside the pipe.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Sunday, January 31, 2016 9:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Galvanized in 1986 wet system

It states it was a wet system, so the c-factor would not have been an
influence.  I think Todd hit it on the head...extra materials in shop to go
through.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/31/2016 7:03 PM, Vince Sabolik wrote:
> If there is a pattern it was probably done for a better c factor - 120 vs
100. I did some like this.
>
> On Jan 31, 2016, Todd Williams <fpdcdes...@gmail.com> wrote:
>> Sounds like someone may have needed to clean out the shop. Are the 
>> pieces randomly installed or is there a pattern?
>>
>> Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
>> 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic 
>> [https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2]
>> On Sun, Jan 31, 2016 at 8:42 PM, 
>> sprinklerforum@lists.firesprinkler.org
>> <sprinklerforum@lists.firesprinkler.org> wrote:
>> Gentlemen,
>> I have never seen this before. There is a mixture of galvanized and 
>> black steel pipe used in a wet system in a normal circa 1986 4-story 
>> office building in the Southeast.
>>
>> Because I have never seen this before in thousands of buildings, I am 
>> assuming that this is a problem.
>>
>> Does anyone have further information?
>>
>> Thank you for your insight.
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> Somehow, Verizon got this to you!
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Locker Rooms

2016-01-05 Thread Art Tiroly
I think the allowable storage in light hazard occupancy is 6-7Ft. 
Think about a light hazard library with rows of book shelves.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of aaron rohr
Sent: Monday, January 04, 2016 9:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Locker Rooms

Really,
Ask him if he wants all cabinets to be covered by OH1?  Do you think the heads 
are listed for closed compartments? Is NFPA 13 intended to cover every space? 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Calcs with soffits

2016-01-05 Thread Art Tiroly
We have a discussion about sidewall and pendant sprinklers in a 36" x 16"
soffit that surrounds a dorm rooms in a jail.

Do the QR pendant sprinklers need to be calculated with the QR sidewall
sprinklers in the 900 SF area? We have 14 sprinklers flowing in areas that
seems excessive and not required. Can't find where this covered in 13.

Appreciate your help.

Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell






---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Calcs with soffits

2016-01-05 Thread Art Tiroly
We are required to install 5.6K Institutional sprinklers due to jail
occupancy. 
The pendant sprinklers are 16" below the ceiling. The room would need to be
an inferno to fuse all the pendants.
Any other opinions please. 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack
Sent: Tuesday, January 05, 2016 12:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Calcs with soffits

Can you use 4.2 or 2.8k sprinklers to cut down discharge? 

I don't think anything in 13 will say not to calc all in a room. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Jan 5, 2016, at 10:32 AM, Art Tiroly <atir...@atcofirepro.com> wrote:
> 
> We have a discussion about sidewall and pendant sprinklers in a 36" x 16"
> soffit that surrounds a dorm rooms in a jail.
> 
> Do the QR pendant sprinklers need to be calculated with the QR 
> sidewall sprinklers in the 900 SF area? We have 14 sprinklers flowing 
> in areas that seems excessive and not required. Can't find where this
covered in 13.
> 
> Appreciate your help.
> 
> Art Tiroly
> ATCO Fire Protection/Tiroly
> 24400 Highland Rd CLE 44143
> 216-621-8899
> 216-570-7030 cell
> 
> 
> 
> 
> 
> 
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flow test - Playpipe w/ 1 1/4 Tips

2015-05-13 Thread Art Tiroly
How did you get a pitot higher than the residual?  Can't happen. Gage error?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Colin Carew (Cambridge)
Sent: Wednesday, May 13, 2015 11:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

Hey Brad for sure , 

Our first test static and residual -  73 / 68 with 75 pito on play pipe with
1¼ tip 
2nd test static and residual -   74 / 69  and my flow after coefficient is
right in line with yours !   


We did the test at approximately the same time 9pm at night .  hydrants were
on 12 main  ( mains are less than 10 years old and on loop . )

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: May-13-15 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

Thanks!

If the Coefficient of Discharge for a 'pollard diffuser' is .9---

h= 42/.433=97 ft
v=(2gh)^.5=79 ft/sec

((2.5/24)^2)*pi= .034 ft^2, * 79 ft/sec= 2.69 ft^3/sec, *7.48*60= 1207 GPM,
* .9= 1086 GPM. (using 29.84*c*d^2*p^.5 gives 1088 GPM, but I like seeing
the velocity, and I rounded down).

Without the static and residual for both though we cannot compare the
graphs, which is what I was interested in. Would it be too 'proprietary' to
post those? Even though the gauged hydrant did not change elevation between
the two tests, it is possible (and likely) there was different amounts of
domestic use during the tests.

Roland, before you have to nip me in the bud again I want you to know I am
not trying to make this thread a clearing house for tons of water flow data
:) 

Brad

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Colin Carew (Cambridge)
Sent: Wednesday, May 13, 2015 6:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

New flow test results - 

2½ pollard diffuser - Pito of 42 - 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: May-07-15 10:33 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

you're welcome!
please post the static, residual, and flow here from both tests-- it would
be informative to see how they compare!!!

Brad

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Colin Carew (Cambridge)
Sent: Thursday, May 07, 2015 9:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

Its ordinary Group 2 ,  based on just that 300 for the system demand . I
used the in-correct coefficient .  thanks !   
I am going to do another test , luckily in my bad luck  this is close to my
office . 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: May-07-15 10:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

What is your estimated demand?

Coefficient of Discharge for playpipes is .97---

h= 70/.433=161.66 ft
v=(2gh)^.5=102.03 ft/sec

((1.25/24)^2)*pi= .008522 ft^2, * 102.03 ft/sec= .8695 ft^3/sec, *7.48*60=
390 GPM, * .97= 379 GPM.

Brad

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Colin Carew (Cambridge)
Sent: Thursday, May 07, 2015 9:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Flow test - Playpipe w/ 1 1/4 Tips

Hey All ,

I just did a flow test last night .  Instead of flowing just the 2½ butt and
getting the pitot  pressure like I have done for years , We used (1) Play
pipe with 1 1/4 Tip . When I convert the pito of 70  to GPM with the 0.90
Coefficient to = 363.41 GPM .Should I have flowed both sides with two
play pipes to determine a higher flow rate  .  I have an old flow test from
Two years ago that has a flow rate of 1186 Gpm .   I am going to do another
test next week   and just flow the 2½ butt with no playpipes .

Colin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list

RE: Flow test - Playpipe w/ 1 1/4 Tips

2015-05-13 Thread Art Tiroly
I got a flow test with a much higher pitot than residual due to a 51 Ft.
elevation change.

Art
ATCO

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of mphe...@aerofire.com
Sent: Wednesday, May 13, 2015 1:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flow test - Playpipe w/ 1 1/4 Tips

Also, I think you missed what Art said, he was referring to the Pitot
pressure in excess of the residual, and actually, I believe that can happen
when testing with a Playpipe due to the increase in velocity. Or I could
have just made that up steve. :-0 Mark at Aero
602 820-7894

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Wednesday, May 13, 2015 10:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Flow test - Playpipe w/ 1 1/4 Tips

Technically it can happen.  When the supply drops, additional supply pumps
kick on, creating a residual pressure greater than the static.  No guidance
in NFPA 24 in how to address so if one applies a literal read, you
extrapolate toward infinity. It's in the works to address.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On May 13, 2015, at 9:46 AM, Art Tiroly atir...@atcofirepro.com wrote:
 
 How did you get a pitot higher than the residual?  Can't happen. Gage
error?
 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Main Drain Coefficient

2015-04-16 Thread Art Tiroly
Without a pitot at the outlet no way to tell.
You can try to hydraulic calculate the flow through the 2 valve, ells and
pipe length using static/residual psi at the riser.

Art

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jeremy Frazier
Sent: Thursday, April 16, 2015 3:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Main Drain Coefficient

I understand the intent, however I need to calculate the gallons. 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Thursday, April 16, 2015 3:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Main Drain Coefficient

It is not the intent of a main drain test to measure the flow, only the
pressure drop.

Steve L.




-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jeremy Frazier
Sent: Thursday, April 16, 2015 12:18 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Main Drain Coefficient

Is it necessary to use a coefficient for a main drain test like you do on a
fire hydrant?  I know you use the coefficient because the stream doesn't
have a perfect discharge column.  If you do need to use it, what would it be
for a 45° or a 90°?

 

Jeremy Frazier

P:571-931-1004
F:571-931-1010

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: MAPP Construction

2015-04-03 Thread Art Tiroly
Who is MAPP Construction?
Who is the AHJ?

Art

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of proud-texan
Sent: Friday, April 03, 2015 10:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: MAPP Construction

If any of you have had experience with a GC called MAPP Construction please
contact me off forum.  Your experience and  evaluation would be greatly
appreciated because they are demanding that we deviate from NFPA and are
holding $$ because we will not. (bship...@mmmpha.com)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Stainless Steel pipe in sprinkler systems

2015-04-02 Thread Art Tiroly
The problem may be joining pipe and outlets. What about copper?


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Morey, Mike
Sent: Thursday, April 02, 2015 9:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Stainless Steel pipe in sprinkler systems

I'm sure this has been addressed but I'm not finding it after some
searching, are there stainless pipes that fall into the general approvals of
NFPA 13 (I don't have full access to ASTM/ANSI but the stuff called out in
NFPA 13 doesn't seem to be for stainless pipe), or is there specifically
approved stainless pipe/fittings for sprinkler work?  Or will we need to get
a variance based on it being better?  We're working in a clean environment
and are probably going to provide socket weld fittings or threaded fittings
and back weld them (other than the heads obviously).  Socket weld fittings
are mentioned, but the only mention of stainless anywhere in the standard is
the C factor table.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
mo...@bmwc.comhttps://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDt
QSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.URL=mailto%3amanta%40b
mwc.com |
www.bmwc.comhttps://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQS
kfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.URL=http%3a%2f%2fwww.bmw
c.com%2f
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org