Would this be similar to baled corrugated box board?
These are very dense bundles that can only allow a surface burning.
Yes it's class 3.
Is this stacked on the floor in large piles or in racks?
NFPA 13 should have the answer.
Art
From: James Crawford
Sent: Friday, March 10, 2023
Some of the new 5” hose in the bed of the truck is plastic covered flexible
material.
Art Tiroly
From: Brett Peters
Sent: Thursday, February 16, 2023 4:47 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Fire Station
Using an ESFR sprinkler at 100 GPM for 12 sprinklers may be more of a cost
savings.
Art
From: Trillium Fire Sprinkler Design INC
Sent: Saturday, December 03, 2022 7:53 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] Re: NFPA 21 VERSUS
Message-
From: Art Tiroly
Sent: Thursday, September 15, 2022 12:22 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] Re: Fire pump package weight ?
What GPM and what HP?
-Original Message-
From: Sean Lockyer
Sent: Thursday, September
What GPM and what HP?
-Original Message-
From: Sean Lockyer
Sent: Thursday, September 15, 2022 12:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Fire pump package weight ?
About how much would you surmise the weight of an electric horizontal
split-case fire
The high pressure water in=rush compresses the air in the system.
The velocity slows as the air pressure is compressed. I don't believe there
is water hammer potential because the air creates a cushion.
Art Tiroly
ATCO/Tiroly Fire Protection
-Original Message-
From: Sprinklerforum
Is the spill container open top? That will be an issue. These sound like
plastic totes. If the liquid is not combustible the empty tote is still a
lot of plastic
Art
-Original Message-
From: Sprinklerforum On
Behalf Of Scott Futrell via Sprinklerforum
Sent: Wednesday, January 26, 2022
.
Art Tiroly
ATCO Fire Protection
-Original Message-
From: Sprinklerforum On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey
Subject: Attic protection over a storage occupancy
Applicable code
I had a similar problem but worked it out with AHJ and he allowed the
obstructions with the ESFR's.
Art Tiroly
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford via Sprinklerforum
Sent: Monday, February 01, 2021 12
For a home worth multiple millions a 10 minute water supply for life safety may
not be the best answer for property values.
There may be insurance savings to help pay for the extra cost for 13R.
Local requirements for high value homes may be the better value for the
sprinkler system.
Art Tiroly
What does the building code say regarding this construction and occupancy?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Larrimer
Check with the AHJ. I’m not sure you can change from 13 to 13R in the same
building. You can use residential rules in a 13 system of course. Do you have
combustible concealed spaces in the residential?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216
Residential use above a parking garage changes the occupancy requirement to
a mixed use and NFPA 13 design criteria is required. Therefore protect the
garage. Am I on the right track here?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
ESFR hose allowance is 250 gpm.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Trillium Fire Sprinkler Design Inc. via Sprinklerforum
The exposed plastic milk crates drive this into the exposed plastic storage
hazard.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf
properly.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Skyler Bilbo
Sent: Friday, March 22, 2019 5:33 PM
To: sprinklerforum
Would the well be considered as potable drining water?
Particulates are the problem.
If the well draws on a lot of sand it is likely raw water.
What is the likelihood of particulates plugging a 1" sprinkler?
You could add a strainer to remove particulates.
Art Tiroly
ATCO
I recently did a system upgrade of an OH pipe schedule system with 130
SF/head..
Good water supply and a low storage height made it work easily.
Back then only hazardous liquids were designed to extra hazard pipe schedule
and K8 - 90 SF/head.
Art Tiroly
ATCO Fire Protection/Tiroly
Due to the change of occupancy the sprinkler system should match the
requirements of the new occupancy.
If quick response sprinklers are required for code compliance then they need
to be changed.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030
What is storage class?
How wide are shelves for picking. Solid shelves?
Are there possible obstructions on the walkways?
How high is each level?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Roland Huggins
Sent: Monday, October 29, 2018 6:42 PM
To: sprinklerforum@lists.firesprinkler.org
What is the sprinkler spacing 90-130 SF?
Light or OH?
Not meant for warehousing.
I'm working on one now converting from factory to warehousing.
1”, 1”, 1-1/4” does not calculate at 130 SF/head.
Up sizing to get .20/1500 for 8-10’ storage of household furnishings and
storage.
Art
Can the ESFR's be left in place and just add in rack sprinklers as needed?
Art
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery
Sent: Monday, October 08, 2018 7:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL]
sprinklers head links near those that actuated.
Links will start to fail with the link solder cracking
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf
What is city water static pressure?
What is the pressure when pump is running?
Likely an omission by installer.
Could it have been removed?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
They will allow car storage with fuel in the tank.
Metal partitions will easily transmit heat to the adjacent unit.
No propane tanks.
Corp allowed to store overflow stock or equipment.
40,000 SF in low bay.
Corridors will have drop ceilings with pendant sprinklers.
Art Tiroly
ATCO Fire
schedule system is not adequate for the hazard.
The sprinkler system should be revised and brought up to NFPA design
density.
Is the appropriate design based on Class A plastic or something less?
I could not find anything in archives.
Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE
Two rows of in-rack sprinklers may solve the rack problem.
Art Tiroly
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf
Of John Irwin
Sent: Thursday, May 17, 2018 11:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Misc Rack S
What is the fire flow test for this system?
What size is the underground fire line.
What size is the riser to be.?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
Are the aisles narrow like 30-48”?
The cat walks are likely considered obstruction to the ESFR roof system.
Therefore QR sprinklers are required below the cat walks.
See Section 20.7.3. for ESFR. Does this qualify with these 10 requirements?
Art Tiroly
ATCO Fire Protection/Tiroly
24400
Creating a PVC drain header for the branch lines should not be done.
Same reason as not running PVC with sprinkler head tees. Not an approved
material.
Art Tiroly
ATCO Fire Protection
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Scott Futrel
How is the butane contained In steel high pressure cylinders or something
larger?
If the vessels are kept cool with water spray during a fire then it is safe.
Leaks could have flash or explosion hazards potential.
Need more info.
Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216
Using 5.6K QR heads will change the hydraulic calculations and minimum flows
allowed by residential sprinklers.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun
I believe that means a HE foam system plus a sprinkler system with a .30
density.
Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf
Check out the residential rules in NFPA 13, Section 8.4.5. Similar to 13-R.
4 heads.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf
In our jurisdiction the backflow would be required where it enters the building
from underground.
A long run of black steel pipe is not allowed without a BFP assembly.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From
Is this a residential or light hazard 8 story building?
Do you have a 1000 gpm fire pump from city water? Electric or diesel?
Reliable power with no outages?
3 - 4 or more standpipe risers?
Then you can get answers.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
Trapeze to spread the load?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:33 PM
An recent arson car fire beneath a bridge structure caused the collapse of the
steel structure and bridge deck on I-85 in Atlanta.
It will take months to repair.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
mack
On 6/13/2017 3:08 PM, rongreenman . wrote:
Just figure a lot per foot, double it, and then add on the extras.
On Tue, Jun 13, 2017 at 3:05 PM, Art Tiroly <atir...@atcofirepro.com> wrote:
Thanks.
How do you determine the cost of operating a heat trace system?
That is important
managers.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack, SET
Sent: Tuesday, June 13, 2017 6:25 PM
To: sprinklerforum
Subject: Re: Heating cable and 1" wrap.
If ceiling is too costly wait until you see the price of heat tracing an entire
system.
On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly <atir...@atcofirepro.com> wrote:
They need store packaging material, idle pallets.
Ceiling is also
Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
craig.pr...@ch2m.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Tuesday, J
cable and 1" wrap.
What are they storing?
Could they put in a false ceiling?
Matt
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: He
think it is a mistake due to reliability and cost
There must be reasons this heating method is not being installed on a
sprinkler system.
What arguments can I use to avoid this method of keeping a wet grid system
from freezing.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE
I saw it done some years ago by pipe fitters and it made me laugh.
The fittings were below the concrete floor so they gouged to floor for the
flanges.
If you need to go back underground the ell won’t fit at the floor.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
I have seen a seen steam turbine driven fire pump about 30 years ago.
Call a fire pump rep and they should know.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
A safer solvent wash tank would have an automatic closing lid actuated by a
fusible link.
Would a Stoddard solvent with a flash point over 100*F be acceptable?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
You could make PDF's details from AutoCAD drawings to add to documents.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott
Get a 3000 gpm flow test with multiple hydrants as required. What size is
the city main?
With 180 gpm per head you need bigger pipe to lower pump pressure.
(I do hydraulic analysis to solve problems like this.)
Art
From: Sprinklerforum
The LP-46 only requires 15-20 psi end head.
I don't understand the excessive pressure you require.
The 58/56/1583 is a great suction source.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
Is that the total duct length or is there a riser to the roof?
Are there heads in the plenum behind the filter?
Where is the exhaust fan?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
If it is covered with gravel and there is no exposed combustible material then
could a fire propagate in this concealed space?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
Is it a flat roof?
Is it covered with gravel or stone?
If it is built of felt paper and asphalt/tar it will burn.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
ant supplied from the proposed 4” main?
If yes then the main shall be 6”.
Best analysis is to do a preliminary hydraulic calculation to determine if 4”
is adequate.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
F
How much movement where dock connects to shore?
Metraflex Co has flex U loop that may be of value.
Can you support pipe on the floor outside the hand rail?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From
Art Tiroly
ATCO Fire Protection
216-570-7030
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack
Sent: Saturday, February 11, 2017 2:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Commodity class upgrade?
I have a project
Is this an enclosure.
Access door like a closet.?
Electrical equipment?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Dewayne Martinez
ESFR heads require flue spaces 9' apart and no solid shelves.
Solid shelves or no flues may require in-rack sprinkles.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
Review all the obstruction rules.
It should become clear.
18” from storage to deflector is required.
There are also distance to wall obstructions that may be helpful.
I don’t have 13 available at home.
Art Tiroly
ATCO Fire Protection
2126-570-7030
: Sprinklerforum
Hose demand is usually not art of the equation with good city hydrant supply
available.
If you omit hose than it all works.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun
Local code determines when and where protection is required.
NFPA shows how it is to be done.
Art Tiroly
ATCO Fire Pro
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Owen Evans
Sent: Monday, January 23, 2017 12:26 PM
To: sprinklerforum
A worst case would be quantity of flammable liquids.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of wmens...@comcast.net
Sent: Monday
What is RCMP?
Is the skylight less than 3 Ft high?
Is the volume less than 1000 Cu.Ft.?
If yes to both no sprinklers are required in the skylight.
Art Tiroly
ATCO Fire/Tiroly
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of P
Measure the ID of the brass nipple.
The ID is near 1”.
Can you get a 1x3/4 male reducer. Think about velocity and turbulence at ~ 125
gpm
Art
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum
off the wall.”
Larry Keeping
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Art Tiroly
Sent: October-20-16 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprikler obstruction.
What is the reasoning for the 4” minimum space to a w
s to do with pattern development, splash back from the wall
interference. This is sitting in my bucket of potential to probably old
fitters' (wives') tales until I get confirmation from more
reliable/knowledgeable sources than the guy that told me this.
On Thu, Oct 20, 2016 at 6:41 AM, Art
rules are pretty clear. Unless you can find a sprinkler who's listing negates
these rules you're stuck.
On Wed, Oct 19, 2016 at 2:26 PM, Art Tiroly <atir...@atcofirepro.com
<mailto:atir...@atcofirepro.com> > wrote:
12x16” Duct is tight to ceiling.
Up right Sprinkler is about 6” from ceilin
-boun...@lists.firesprinkler.org] En
nombre de IPA
Enviado el: miércoles, 19 de octubre de 2016 02:02 p. m.
Para: sprinklerforum@lists.firesprinkler.org
Asunto: Re: Sprikler obstruction.
Is the duct below the sprinkler deflector?
On Wed, Oct 19, 2016 at 12:25 PM, Art Tiroly <a
Does an upright sprinkler have to be moved when a new duct was added less
than 4" away from the existing sprinkler.
I understand when a new sprinkler is installed it shall be 4" away from a
wall.
I have adequate coverage from the adjacent sprinkler in this basement
meeting room spac
You will also have to meet local code requirements per NFPA 13 for submittal
whichever is geater.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org
Sprinklers above the egg crate will have obstructed flow spray pattern.
How far below the deck are the sprinklers in the egg crate ceiling?
If more than 12"???
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
area with no sprinklers.
Depends on the shape of the pocket.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET
Sent: Tuesday
Thank you. Some of the window pockets are 30-50 Ft. long but still under 1000
Cu.Ft..
Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be the
prime consideration not a 4Ft high pocket along an outside window wall.
Art Tiroly
ATCO Fire Protection/Tiroly
24400
Thank you. Some of the window pockets are 30-50 Ft. long but still under 1000
Cu.Ft..
Old ceiling was 14 Ft. Drop ceiling is 10 Ft. It seems the volume should be the
prime consideration not a 4Ft high pocket along an outside window wall.
Art Tiroly
ATCO Fire Protection/Tiroly
24400
for the fire 8-12
Ft. away. I plan to ask for a variance from the Ohio State plans examiner at
submittal though likely to no avail.
Art Tiroly
ATCO Fire Protection
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brad Casterline
Sent: Monday
He intent is to use either 8.7.7 or 8.8.7 for large pockets.
The volume of the pocket seems more important than the depth.
A 4x4x40-50' pocket should not need sprinklers next to glass windows.
Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
are less than 1000 Cu.Ft.
I don't understand the restriction to 3 Ft. since the air volume seems to be
the relevant restriction.
Do I need to add sprinklers to a ceiling pocket along the windows when I
have floor coverage.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
Sorry for the repetition. I did not think this was getting through.
Art
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Wednesday, July 13, 2016 3:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE:
We have an issue with sprinkler
throat and seal.
There is also an glycerin antifreeze system that does not have this problem.
Suggestions please
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
___
Sprinklerforum mailing list
From: Art Tiroly [mailto:atir...@atcofirepro.com]
Sent: Wednesday, July 13, 2016 2:07 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: Leaking sprinkler due to corrosion
We have an issue with sprinkler water becoming acidic 5.5-6 PH.
System is 6 months old. The Bellville seal
not have this problem.
Suggestions please
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
.
Suggestions please
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
Sprinklerforum
What state are you in?
Can I assume you are planning quick response sprinklers.
Then why not 900 SF area of application allowance?
What part of the code is AHJ using for this requirement.
There are residential rules in 13.
Use residential heads with .10 density
Art Tiroly
Tiroly
Water company requires BFP not NFPA 13, 24.
Art Tiroly
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Thursday, June 23, 2016 11:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Two Backflows
I use RPZ
Easy. Calculate GPM through the 1" pipe and fittings in drain line. Doubt you
will 100 gpm.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkle
Design requirements are in NFPA 30.
How high is storage?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of James Crawford
Sent
Sometimes you have to wake me up. I just saw this question.
Went to google. Tyco uses EC #'s. I saw EC 5, 8, 11, 14 but no EC 10 in
there listing.
Call Tyco they can help. What size is pipe thread. 1/2 or 3/4"?
Art
-Original Message-
From: Sprinklerforum
What is the sprinkler spacing?
Staggered spacing was quite common before 1940.
Newer heads installed?
High pressure water supply connected?
It likely will barely do .10 density or maybe .15 with moderate pressure.
FM used to allow 3-5 psi at end head for pipe schedule.
Art Tiroly
ATCO Fire
Sprinklers don't spray upward. If Foam plastic insul is combustible it burns
faster
than the sprinklers can operate and water is not sprayed upward.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From
the public water pressure
Art Tiroly
ATCO Fire Protection
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd Williams
Sent: Tuesday, February 16, 2016 11:26 AM
Some threadable light wall pipe was galvanized on the outer pipe wall but
not inside the pipe.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun
I think the allowable storage in light hazard occupancy is 6-7Ft.
Think about a light hazard library with rows of book shelves.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum
excessive and not required. Can't find where this covered in 13.
Appreciate your help.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com
room.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
> On Jan 5, 2016, at 10:32 AM, Art Tiroly <atir...@atcofirepro.com
How did you get a pitot higher than the residual? Can't happen. Gage error?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf
.
Roland
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/
On May 13, 2015, at 9:46 AM, Art Tiroly atir...@atcofirepro.com wrote:
How did you get a pitot higher
Without a pitot at the outlet no way to tell.
You can try to hydraulic calculate the flow through the 2 valve, ells and
pipe length using static/residual psi at the riser.
Art
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of
Who is MAPP Construction?
Who is the AHJ?
Art
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of proud-texan
Sent: Friday, April 03, 2015 10:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: MAPP Construction
If any of
The problem may be joining pipe and outlets. What about copper?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Morey, Mike