2.6.1 of IEC 60950-1 refers to parts of equipment shall be reliably connected to the main protective earthing terminal.A hinge would certainly not be regarded as a reliable connection. As far as your door is concerned, is there any single insulated hazardous voltage wiring likely to contact

RE: Security and Alarm Systems

2003-11-14 Thread Crabb, John
A limited amount of information may be found in CENELEC Report R079-001:1998 Guide to achieving compliance with EC directives for alarm systems I don't have a copy, however. Regards, John Crabb, (Product Safety) , NCR Financial Solutions Group Ltd., Discovery Centre, 3 Fulton Road,

RE: LCD Displays and Safety

2003-09-09 Thread Crabb, John
You will have noted in IEC 60950-1 Clause 4.2.5 Impact Test, that it states the test is not applied to flat panel displays or to the platen glass of equipment (for example, copying machines). The waiver for flat panel displays appeared in the third edition of IEC 60950 - some time ago I trawled

RE: New EU Member States

2003-05-15 Thread Crabb, John
As a matter of interest, I have read that the enlargement of the EU is going to provide many, many jobs as translators, and there are anticipated to be major problems ahead since for some language combinations it is expected that there is no-one trained as a translator, and therefore they would

RE: Crossed out wheelie bin symbol (WEEE Directive)

2003-03-31 Thread Crabb, John
In directive 93/86/EEC (relating to batteries containing certain dangerous substances), it says the symbol shall cover 3% of the area of the largest side of the battery or accumulator, up to a maximum size of 5 cm x 5 cm. For cylinrical cells the symbol shall 3% of half the surface area of the

RE: 230V Transition for EU?

2003-02-07 Thread Crabb, John
Cenelec document HD 472 S1, 1989, nominal voltages for low voltage public electricity supply systems is the document that states for the first step, namely to 230V +10% -6%, Note: The dead-line for the completion of the first step is envisaged for 1995. It also states that The transition period

RE: Mercury and Europe

2002-11-06 Thread Crabb, John
Annex ZC (Informative) A-Deviations, in EN 60950-1, states Clause 1.5.1 Deviation Sweden (Ordinance 1990:944) Add the following: NOTE In Sweden, switches containing mercury such as thermostats, relays and level controllers are not allowed. Switzerland (Ordinance on environmentally hazardous

Use of pre-plated steel.

2002-10-02 Thread Crabb, John
Has anyone encountered problems in the use of pre-plated sheet steel in IT equipment metalwork ? Typically such material is cheaper to use than having to plate parts after they have been produced, but there may be issues with sharp edges produced when the material is punched out, and with rust

RE: Water + Electricity

2002-09-12 Thread Crabb, John
You can say that electricity in a bathroom can be dangerous, and in the UK, we are very cautious in this respect: You don't have a wall mounted light switch in a bathroom, it is either outside the room, or the light is operated by a pull cord operated switch on the ceiling. You are not allowed to

RE: Banned Substances in Sweden

2002-08-12 Thread Crabb, John
Annex ZC of EN60950-1, IT Equipment - Safety, states: Sweden (Ordinance 1990:944), In Sweden, switches containing mercury such as thermostats, relays and level controllers are not allowed. Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd.,

RE: Liquid Nitrogen Safety

2002-08-06 Thread Crabb, John
This is way out of my normal range of Product Safety experience, but I can say BE VERY CAREFUL with liquid nitrogen. My memory bank reminded of a fatality in Scotland not that long ago, and after a short search on liquid+nitrogen+death, I came up with the following :

RE: Compliance Primer

2002-07-31 Thread Crabb, John
I agree with Rich on the moral obligation a company has to avoid injury to those who use its products. Every year I give a lecture on Product Safety to manufacturing engineering students at our local university. This is what I say in answer to Why have Product Safety ? - As well as the

RE: IEC60320

2002-07-22 Thread Crabb, John
I have never heard of an inlet with provision for a spare fuse. Are you sure it wasn't a double pole fused inlet ? (SOME PEOPLE say double pole fusing is a requirement of IEC 60950, but it ain't necessarily so). Regards, John Crabb, NCR Financial Solutions Group Ltd., Discovery Centre, 3

RE: TOUCH CURRENT LIMIT

2002-07-09 Thread Crabb, John
Rich Nute said : - For grounded (Class I) equipment for the home, the UL leakage current is 0.5 mA. (This is NOT a 60950 limit.) UL reasoned that if 0.5 mA arises from both real and stray capacitance, then, for double-insulated (Class II) equipment, the current should be one-half of 0.5 mA

RE: SI Unit for volume

2002-06-21 Thread Crabb, John
Answer is presumably in ISO 1000, specification for SI units and recommendations for the use of their multiples and of certain other units. Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Discovery Centre, 3 Fulton Road, Dundee,

RE: Constant for Change of Resistance formula.

2002-05-14 Thread Crabb, John
The formula for calculating the temperature rise of a winding can be found in Annex E of IEC 60950 - and all the experts in TC 74 can't be wrong ?? (I also found the same formula in my 1985 issue of IEC 380. Different temperature coefficents for copper have been quoted, and as far as I can

RE: Constant for Change of Resistance formula.

2002-05-13 Thread Crabb, John
If you plot resistance of copper vertically, against temperature horizontally, and extend the graph backwards, the point of intersection with the horizontal axis is found to be -234.5 degrees C. (Got this out of my early years text book which I keep at my desk !) Hence for a standard copper

RE: IEC 60601-2-24 / Magnetic Field

2002-05-02 Thread Crabb, John
I can imagine that it is a perfectly reasonable requirement that electricity meters be required to operate correctly when subjected to high magnetic fields, to overcome any likely fraud attempts by enterprising consumers with permanent magnets, trying to reduce their electricity bills. I suspect

RE:Draft BS ISO/IEC 17024, certification schemes for persons .

2002-03-27 Thread Crabb, John
I have just obtained the above draft for public comment, which is the BS implemenation of Draft International Standard ISO/IEC 17024 General requirements for bodies operating certification schemes for persons. Apparently the circulation of this draft ISO/IEC standard is also a CEN(ELEC) parallel

RE: IP Rating and EN60950

2002-03-26 Thread Crabb, John
1.1.2 of EN 60950-1:2001 states requirements additional to those specified in this standard may be necessary for .. equipment intended for use where ingress of water is possible; for guidance on such requirements and on relevant testing, see annex T. Annex T, which refers to IEC 60529, is

RE: chassis bonding - star washers enough?

2002-03-25 Thread Crabb, John
: 25 March 2002 15:28 To: Crabb, John Cc: emc-p...@ieee.org Subject: RE: chassis bonding - star washers enough? Hi John, You wrote: We use screws which have combined hex/posidriv heads with serrations under the head, which eliminates the need for star washers. We find these work very well for zinc

RE: LED Color

2002-03-22 Thread Crabb, John
Clause 1.7.8.2 Colours, of IEC 60950-1 states Where safety is involved, colours of controls and indicators shall comply with IEC 60073. Where colours are used for functional controls or indicators, any colour, including red, is permitted provided that it is clear that safety is not involved.

RE: Wire spool labeling requirements

2002-03-14 Thread Crabb, John
Surely the requirement is as found in the Guideinfo for CCN (AVLV2) Appliance Wiring Material, namely ; The Recognition Mark of Underwriters Laboratories, Inc. (illustrated below) on the attached tag, the reel or the smallest unit container in which the product is packaged is the only met.. -

RE: South Korean Power System

2002-02-20 Thread Crabb, John
IEC60950 has a requirement (1.6.4) that the neutral conductor, if any, shall be insulated from earth and from the BODY throughout the equipment as if it were a line conductor. Components connected between neutral and earth shall be rated for the line-to-neutral voltage. Typically I would expect

RE: Japan mains voltage

2002-02-20 Thread Crabb, John
According to World Electricity Supplies from BSI, voltage is 200/100, 60 Hz. We have certainly produced 100V 60 Hz specials for Japan. Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Discovery Centre, 3 Fulton Road, Dundee, Scotland, DD2

RE: Downloadable CENELEC Standards

2002-02-11 Thread Crabb, John
As a matter of interest, when you order a free amendment or corrigendum from BSI, you have a reasonable chance of being supplied with the whole standard !! (which makes my day : ) John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Discovery Centre,

RE: Teslars???

2002-02-08 Thread Crabb, John
There are a series of ENs, 50121, relating to EMC requirements for railway equipment. That's all I know - I just noted in my records back in 1997 that they were starting to appear. I also note in EN 61000-4-8 Power frequency magnetic field immunity, that 1 A/m corresponds to a free space

RE: SV: Generic emissions - EN 61000-6-3

2002-01-30 Thread Crabb, John
I seem to recollect that I have previously pointed out that the LVD states electrical equipment which complies withharmonised standards shall be regardedas complying; and standards shall be regarded as harmonized once they are drawn up by common agreementand published under national

RE: What about 480 VAC in Europe? RE: 2 Phases in North America

2002-01-18 Thread Crabb, John
Just to clarify the position in the UK, although it was stated below that the nominal voltage is 415V, I am almost certain that the DECLARED VOLTAGE is 400V. I base this on the fact that domestic consumers were advised that the declared voltage changed from 240V to 230V, and 230 X 1.732 = 400V,

RE: date of publication relevance to CB Certs

2002-01-17 Thread Crabb, John
I would agree that whether a safety standard is published in the OJ against the LVD should never be an issue. I would remind everyone that the LVD states electrical equipment which complies with the safety provisions of harmonized standards shall be regarded...as complying. FOR PURPOSES OF

RE: CEN Standards free on-line

2002-01-07 Thread Crabb, John
Before we start cutting our budgets for the purchase of standards, I read in another CEN announcement ; eEurope standards are defined in workshops whose agreements will be made available for downloading free of charge from the CEN web site. So it may just be CEN Workshop Agreements (CWAs) that

RE: EN60529

2002-01-03 Thread Crabb, John
John, I have forwarded this information to the chairman of BSI committee EPL/74 (which deals with EN60950), with the suggestion that CENELEC be asked to get EN60529 removed from the list of LVD notified standards. We'll see what happens. On the same subject, TC74 is working on requirements

RE: 2 Phases in North America

2001-12-17 Thread Crabb, John
Bill - you absolutely correct in describing the North American system as single-phase, 3 wire. After all, that is how it is described in Annex V, Figure V.4 of IEC60950:1999 - and there is NO WAY that IEC TC74 could be wrong, is there ? (especially since the US committee must have voted yes, to

RE: ITE equipment in Petrol Station (Gas) outlets

2001-12-05 Thread Crabb, John
ANSI/NFPA 30A is the Automobile and Marine Service Station Code, and has a table of Electrical Equipment Classified Areas - Service Stations, which described the extent of classified areas adjacent to pumps and underground tanks. For our Automated Teller Machines, I always ask the customer to

RE: Mains Cords in the UK and the fuse rating

2001-11-30 Thread Crabb, John
Almost certainly the answer will be found in BS1363 Part 1, Specification for rewirable and non-rewirable 13A fused plugs. (I assume you are referring to UK plugs, as I don't know of any other plug with a fuse). My copy of BS1363 is rather old, but there is a table which shows a 3A (5A) fuse

RE: EMI filter hazards

2001-10-29 Thread Crabb, John
There are many EMI filters on the market with a discharge resistor across line and neutral to discharge the capacitor(s). The filter we use has a one megohm resistor built in. IEC60950 requires that capacitor exceeding 0.1uF should have a means of discharge resulting in a time constant not

RE: skinny power cords.

2001-10-26 Thread Crabb, John
Far be it from me to criticize UL Listed products, or UL standards, but it seems to me that the plug in question was not suitable for its intended use. I can recall conducting a humidity test on one of our products, and at the conclusion of the test, it failed a dielectric test, and I traced the

Photo Sensitive Epilepsy. (PSE)

2001-09-25 Thread Crabb, John
Would anyone have any guidelines on how to design computer graphics in such a way to avoid inducing Photo Sensitive Epilepsy in anyone who suffers from that complaint ? Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West,

RE: Manufacturing Hipot Testing

2001-08-23 Thread Crabb, John
Far be it from me to nit-pick, but to say in a standard that the tests specified in this annex SHOULD be carried out by the manufacturer on each luminaire after production, doesn't sound like a normative requirement. They should have used SHALL. But maybe it is an informative annex ? Regards,

RE: Creepage dist. for more than 1000V ?

2001-08-15 Thread Crabb, John
I hesitate to remind you all, but if anyone has a problem interpreting the requirements of IEC 60950, there is the TC74 Chairman's Advisory Panel. Briefly, the procedure is as follows : Questions for interpretation should, as a minimum - define the problem, making reference to a specific

RE: How Safe ???

2001-07-25 Thread Crabb, John
There are stability tests in UL751 - Vending machines, which I have in my fantastic filing system. (Just in case anyone thought my products - Automated Teller Machines, were vending machines). I can't be sure if they are also in UL541 - Refrigerated Vending machines - since I don't have a copy.

RE: Voltage Range in Asia

2001-06-22 Thread Crabb, John
Figures I have entered below are from the 1996 edition of the BSI publication World Electricity Supplies. Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West, Dundee, Scotland. DD2 3XX E-Mail :john.cr...@scotland.ncr.com Tel:

RE: Protective Bonding-UL 60950 (replacement for UL 1950)

2001-05-18 Thread Crabb, John
As a previous reply has suggested, but not in the same words, surely one question that has to be considered is whether this hinged panel is required to be earthed. The requirement in UL60950 2.6.1 a) refers to accessible conductive parts that might assume a HAZARDOUS VOLTAGE in the event of a

RE: US Mains Plug/Earthing

2001-05-17 Thread Crabb, John
I don't know if you have to fit a plug, but I can certainly tell you that our USA customers would be VERY UNHAPPY if we supplied a product without a plug. I certainly have the impression that fitting a plug in the USA is not something that people expect to have to do. Regards, John Crabb,

RE: Classification of Office Equipment

2001-02-21 Thread Crabb, John
The scope of EN60950 Safety of IT Equipment reads : SAFETY OF INFORMATION TECHNOLOGY EQUIPMENT - 1 General 1.1 Scope 1.1.1 Equipment covered by this standard This standard is applicable to mains-powered or battery-powered information technology equipment, including electrical business equipment

RE: FLAME RATING OF STANDOFFS

2001-02-20 Thread Crabb, John
I certainly have a lot of small plastic parts in my products which I consider to be exempt and are not described in any procedure - and they may well be a lot bigger than your standoff !! I certainly think your agency is not-picking !! One point to consider is that I write the procedure for UL

RE: 230 Vac or 240 Vac?

2001-02-13 Thread Crabb, John
I cannot answer for all the countries involved, but I can quote the document which was delivered to my home address in 1995 from my electricity supplier (Scottish Hydro-Electric), and which, naturally, I brought into work and filed under 230V harmonization : - DECLARED NOMINAL SUPPLY VOLTAGE

RE: Client Presence During Testing

2001-01-24 Thread Crabb, John
We are fortunate in that we always get the lab personnel to come to our facility to test our products. This has many advantages, the main ones being that any issues can be cleared up with the design engineers, and you don't let the lab people go until they agree to approve your product !!

RE: ECMA standards

2001-01-24 Thread Crabb, John
The ECMA 2000 Memento (their yearly handbook)shows ECMA-97 as withdrawn, with no note of any equivalent international or European standard. There is no copy of ECMA-97 on the CD-ROM distributed with the 2000 ECMA Memento. Unfortunately I have disposed of my previous ECMA CD-ROMs, but maybe

RE: PUWER Directive?

2000-12-14 Thread Crabb, John
This directive states : - that employers must obtain and/or use work equipment which, if provided to workers in the undertaking and/or establishment for the first time after 31 December 1992, complies with the provisions of any relevant Community directive which is applicable. I read this as

RE: International Equivalent of EN50116

2000-12-08 Thread Crabb, John
As a member of the British EPL/74 committee, I can say that I know of no plans to issue an IEC standard equivalent to EN50116. Historically, almost certainly ECMA will have produced their standard and then given it to CENELEC who issued it as EN50116. I don't know if IEC would entertain

RE: End of Line Testing of IT Equipment

2000-11-29 Thread Crabb, John
I'm sure we have been through this all before, but here goes : For equipment certified by UL and CSA (and I assume by other agencies, but I have no personal experience), the End of Line Tests will be specified as part of your certification. For Europe, there is EN 50116, which defines the

RE: Rechargeable Batteries

2000-11-24 Thread Crabb, John
One reason I have heard - and I can't recall where, was simply that the equipment (in particular - toys) had originally been tested and found to comply with the appropriate requirements, when tested with zinc carbon batteries, and manufacturers are loath to claim that their equipment is ok

RE: safe voltage limits for cattle ( cows horses etc)

2000-11-10 Thread Crabb, John
Try EN 61011, Electric fence energizers. Safety requirements for mains-operated electric fence energizers. EN 61011-1 Safety requirements for battery-operated electric fence energizers suitable for connection to the supply mains. EN61011-2 Safety requirements for battery-operated electric fence

RE: Directive 96/29/euratom

2000-11-09 Thread Crabb, John
URL for required Directive - happy reading ! http://europa.eu.int/eur-lex/en/lif/dat/1996/en_396L0029.html John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West, Dundee, Scotland. DD2 3XX E-Mail :john.cr...@scotland.ncr.com Tel: +44

RE: Directive 96/29/euratom

2000-11-09 Thread Crabb, John
In the latest edition of EN 60950:2000, Safety of IT Equipment, Annex H, Ionizing Radiation, you will find the following changed text : - At any point 10cm from the surface of the OPERATOR ACCESS AREA, the dose rate shall not exceed 1uSv/h (0.1 mR/h) (see note). Account is taken of the

RE: Correlation of UL 1950 and DIN EN 60950 (VDE 0805) also EN/ IEC 60721-3-3 (-2)

2000-05-10 Thread Crabb, John
EN 60721-3 = Classification of groups of environmental parameters and their severities. According to the BSI catalogue, EN 60721-3-2 is identical to IEC 60721-3-2, Transportation, defines conditions to which a product is subjected while being transported from one place to another after being

RE: Indicator Color and Safety

2000-03-23 Thread Crabb, John
The use of the colour red for on/off switches is now enshrined in history, and I see no reason to outlaw the practice, provided it does not create a hazard. ( I must be getting old, if I am starting to use the it has always been this way argument). Looking in catalogues for switches in common

RE: Inquiry on Restrictions and Bans of Mercury in Product compon ents

2000-01-17 Thread Crabb, John
)1382-592289 (direct ). Fax +44 (0)1382-622243. VoicePlus 6-341-2289. -Original Message- From: Paul J Smith [SMTP:paul_j_sm...@notes.teradyne.com] Sent: 07 January 2000 17:13 To: Crabb, John Cc: emc-p...@ieee.org Subject: RE: Inquiry on Restrictions and Bans of Mercury

RE: Y2K glitch

2000-01-17 Thread Crabb, John
As the worlds No. 1 manufacturer of ATMs, and probably the manufacturer of the ATM in question, I have received the following information from our people in Hungary : - The scanned ATM receipt is NOT REAL, the date on it had been manually altered, but it is not a good joke, it is a serious

RE: Handheld tool display window

1999-12-02 Thread Crabb, John
As a manufacturer of Automated Teller Machines (ATMs) which are subject to considerable mechanical abuse, we have not found any particular standards detailing tests for such abuse. There are requirements for impact tests for the exterior of enclosures which would give access to hazards, in IEC

RE: Earth Leakage Measurement Circuit per EN 60950

1999-11-29 Thread Crabb, John
I use a Yokogawa Type 3226 Universal Leakage Current Meter which is quite old, (10 years ++) and can measure ac current, dc current, and dc+ac current, with input resistances of 1, 1.5 and 2 kohms. I also have a Simpson 229-2 (also quite old) which gives me very similar results to the above.

RE: Supply tolerance for Brazil

1999-11-22 Thread Crabb, John
World Electricity Supplies (from BSI) gives household voltage as 220/127V, +5%. -7.5%. John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West, Dundee, Scotland. DD2 3XX E-Mail :john.cr...@scotland.ncr.com Tel: +44 (0)1382-592289 (direct ).

RE: Non flammable material

1999-11-18 Thread Crabb, John
From IEC 74/510/CD, draft amendment to IEC 60950, Material flammability classifications, HBF replaced by FH-3. The new definitions are not in all cases identical to the earlier ones. I imagine the -40 in the FH3-40 you refer to is the burning rate of 40mm/min specified for HBF. A certain

RE: internet information

1999-11-18 Thread Crabb, John
Sorry to add to the confusion, but the British trade association FEI publishes a document on periodic safety checks for business equipment, which includes a table of conductor sizes and fuse sizes for British plugs, with the following note: BS 1363 specifies only the use of 3 A or 13 A fuses.

RE: Underfloor Radiant Heating Panels for Europe

1999-11-17 Thread Crabb, John
In the BSI catalogue I have found : - BS EN 1264 Floor Heating. Systems and Components comprises : BS EN 1264-1:1998 Definitions and symbols BS EN 1264-2:1998 Determination of the thermal output BS EN 1264-3: 1998 Dimensioning All the above BS are identical to the EN. There is also a BSI CP 1018

RE: European Standards in conflict with the EMC directive

1999-11-12 Thread Crabb, John
I presume you have a copy of PD 6608:1997 = CENELEC REPORT R079-001:1996, Guide to achieving compliance with EC directives for alarm systems. (I don't know if a more up-to-date version exists). I bought this document to see what it said about safety, but it just said EN 60950 shall apply. I am

RE: Operating Tolerance

1999-11-11 Thread Crabb, John
BSI World Electricity Supplies quotes +/-10% for overhead cable and +/-7% for underground cables for 220V in Argentina. For the US, there are tolerances quoted for some cities. Worst is +/-10% for Pittsburgh for power as opposed to lighting. Regards John Crabb, Development Excellence (Product

RE: IEC 127 fuse

1999-09-30 Thread Crabb, John
I am going on vacation (to Florida!) tonight, but just to stir things up, WHY ALL THESE NEVER-ENDING DISCUSSIONS ON IEC127 and UL FUSES. It IS possible to get products approved by UL and European agencies, without using different fuses. We buy power supplies and monitors, with UL and at least

RE: IEC 60990 Vs IEC 60950

1999-09-28 Thread Crabb, John
For my sins, I am on the BSI committee which provides the British input to IEC 60950, and I have every sympathy with you, Nick. I can advise from memory, that the British committee usually tries to ensure that all the requirements end up in IEC 60950, where reasonably practical. I seem to

RE: Re: EN 60 950 and Denmark

1999-09-28 Thread Crabb, John
For everyones information, the wording of the Danish Special National Condition, as found in Annex ZB (normative) of BS EN 60950 = EN 60950 is : Clause 1.2.4.1, In Denmark, certain types of Class 1 appliances (see subclause 3.2.1) may be provided with a plug not establishing earthing

RE: LCD Displays

1999-09-27 Thread Crabb, John
If you perform a limited current test on your inverter, as per IEC 60950 2.4.2, you will probably find it meets these requirements, which means that theoretically Operator access is allowed - though you'll definitely feel it if you touch it :( .However, it does mean that if the invertor output

RE: UL1950 Flammibility Requirements

1999-09-23 Thread Crabb, John
UL1950 states : 4.4.5.2 Components not requiring a fire enclosure -components in a SECONDARY CIRCUIT supplied by a limited power source complying with 2.11, provided that : -the components are mounted on materials of FLAMMABILITY CLASS V-1 or better, and -the wiring used in such circuits is

RE: FW: Double pole fusing

1999-09-16 Thread Crabb, John
I recalled that this subject had been discussed in depth at a BSI committee meeting, but had to dig back to 1995 to find it. The BSI committee stated, in response to any enquiry such as yours : - --- Please be aware that

RE: Suppression capacitors

1999-09-08 Thread Crabb, John
The standard which applies is IEC 60384-14 Fixed capacitors for use in electronic equipment-Part 14, Sectional Specification; Fixed capacitors for electromagnetic interference suppression and connection to the supply mains. I only have a draft in my possession. It states Capacitor of Class X,

RE: Grounding Bond Test

1999-08-26 Thread Crabb, John
The original post said : EN 50116 for ITE specifies the earthing terminal or earthing contact may not exceed 0.1 ohms when 1.5 times the current capacity of hazardous circuits is applied, but not more than 25 A (ac or dc) for 60 seconds. My copy of EN50116 specifies the time as being for the

RE: Equipment designed and manufactured for use in-house

1999-08-13 Thread Crabb, John
Since this is a UK question, The Provision and Use of Work Equipment Regulations 1992 (SI 1992 No. 29323) would seem to apply. It states under Conformity with Community requirements 10 - (1) Every employer shall ensure that any item of work equipment provided for use in the premises or

RE: WEEE Directive

1999-08-05 Thread Crabb, John
Doug, I would have thought you would already have come across the symbol for the crossed-out wheeled bin in the directive 93/86/EEC which adapts to technical progress Council Directive 91/157/EEC on batteries and accumulators containing certain dangerous substances, the dangerous substances being

RE: CSA C22.2 No. 950

1999-07-08 Thread Crabb, John
You could try asking CSA for a copy of their CSA 950/UL1950 Design Manual, which includes a fair amount of the French marking text (and is quite a good short list of basic design requirements). I would expect that this document would be free. I am a little puzzled by a note in the rather old

RE: FDA requirements

1999-06-25 Thread Crabb, John
As far as I am aware, the FDA requirements (21CFR) relate to the emission of X-rays from CRTs within monitors. We always state that any LCD displays within our products are therefore exempt from the FDA requirements. I also have on file a letter to all manufacturers and importers of television

RE: Back-Light Circuit

1999-05-19 Thread Crabb, John
I agree with Rich's suggestion re treating this as a Limited Current Circuit, and carrying out the test in 2.4 with a 2000 ohm resistor. We have done this for several LCD displays we use, to satisfy UL, and they seem happy to accept this. We also short circuit the transformer output to prove

RE: Australian electricity supply

1999-04-29 Thread Crabb, John
My 1996 World Electrical Supplies says 240 V +/- 6% Regards, John Crabb, Development Excellence (Product Safety) , NCR Financial Solutions Group Ltd., Kingsway West, Dundee, Scotland. DD2 3XX E-Mail :john.cr...@scotland.ncr.com Tel: +44 (0)1382-592289 (direct ). Fax +44 (0)1382-622243.

RE: What color is neutral.

1999-04-22 Thread Crabb, John
...@bev.etn.com] Sent: 21 April 1999 16:18 To: 'Crabb, John'; 'discussion group' Subject: RE: What color is neutral. Mr. Crabb, I appreciate your spending 2c (or is that 2p!) on this issue. As the 'thread' initiator, I hope I can trouble you with a follow-up. As you and Mr. John Woodgate

What color is neutral.

1999-04-21 Thread Crabb, John
In our detachable cord connected products, we use American power cords with black, white, green wires on 120V units which are UL Listed, CSA Certified; and European cords with brown, blue, green/yellow wires on 230V units. (As an aside, note how UL and CSA choose to ignore the UL1950 requirement

RE: US/ HAR line Cord

1999-03-24 Thread Crabb, John
I managed to find in the top 6 inches of my in-tray (piled 18 inches high), the Subject 1950 and 1459 letter from UL dated October 26, 1998; Subject: New Issue of Standardized Appendix Pages. These are for ITE (NWGQ), Power Supplies for ITE (QQGQ); Telephone Appliances (WYQQ); and Power Supplies

RE: Leakage Current Measurements

1999-03-12 Thread Crabb, John
We use a Yokogawa 3226 Universal Leakage Current Tester together with a 3227 Test Box. The meter has both an AC and an AC+DC current range, and switchable 1K, 1.5K, and 2K input resistance. The test box has a polarity and an on-off switch to simplify testing, and has a US mains socket into

RE: Company Name Change

1998-12-22 Thread Crabb, John
I have a file at least an inch thick on company name change, since NCR changed to ATT and back again. Certainly it was simple as far as UL and CSA were concerned. For UL you will have to notify them of the change of Listee, Applicant, Manufacturer, etc, as appropriate for each volume of your

RE: CE Requirements for Marine equipment

1998-12-17 Thread Crabb, John
Brian, is case you are concerned by the statement that EN 60945 ...is almost the same as IEC 60945, according to my BSI catalogue, BS EN 60945 (the British implemetation of EN 60945) is identical in every detail to EN 60945 and IEC 60945, therefore EN 60945 and IEC 60945 are identical (in

RE: Harmonized Cordage - meaning

1998-12-17 Thread Crabb, John
Briefly, the HAR mark means the cordage has been approved by one of the members of the CENELEC HAR scheme, whereby cordage is tested to Harmonized standards, and is accepted by all of the members of the scheme without further hassle. A manufacturer can only get a HAR mark if he is in a country

RE: Signatory for US based Manufacturer

1998-12-15 Thread Crabb, John
NCR keeps a copy of the Declarations of Conformance on file in Europe (in London), signed by a legal person (our International Intellectual Properties Counsel) who is based in London. It is also signed by the Director of Operations of the US manufacturing plant. John Crabb, Development Excellence

RE: Questions on Plug Adapters

1998-12-03 Thread Crabb, John
My company (NCR) ships automated teller machines worldwide. Our policy on plugs is simple: - If the product is 120V, we supply a UL/CSA cordset with a NEMA plug, and if the product is 220/230/240V, we supply a HAR cordset, WITHOUT A PLUG, together with a one page chart showing the plugs for

RE: Wiring Requirements

1998-11-23 Thread Crabb, John
The third edition of IEC 60446 Basic and safety principles for man-machine interface, marking and identification - Identification of conductors by colours or numerals is at the FDIS (Final Draft International Standard) stage, with voting terminating on December 15. There is parallel voting for

RE: LED Reqs under A11 to EN60950

1998-11-20 Thread Crabb, John
I would also be interested to know what everyone is doing (or not doing !!). As far as I can gather, everyone is ignoring this issue, as it is just so ridiculous. After all, the only way you can prove that a LED is Class 1 or below is to do the measurements - and I'm sure most of us don't have

RE: Plastics Cert Documentation

1998-11-19 Thread Crabb, John
All we do is to specify the required plastic material by Manufacturer, generic name, and specific grade on our drawings. From time to time, the FUS inspector will pick a part from our assembly line, and check the drawing in our print file to ensure that it calls up a material that meets the UL

RE: Supply Frequency Variations

1998-11-09 Thread Crabb, John
In the BSI publication World Electricity Supplies, 1996 (probably not the latest), the UK variation is given as +/-1%, while the highest given for US (there are different figures for different states) is +/- 0.3%. John Crabb, NCR Financial Solutions Group Ltd, Dundee, Scotland. -Original

RE: Burning Card Module

1998-11-06 Thread Crabb, John
I have come across similar incidents, and guess that the decoupling capacitors have been installed with reversed polarity. The capacitors do not always burst into flame when power is supplied - it may take some time - and if the equipment is not powered up for very long while it is being built

ETSI Standards.

1998-11-05 Thread Crabb, John
Just noticed the following on newsgroup comp.std.internat today: - The European Telecommunication Standards Institute (ETSI) has decided to put all European Telecommunication Standards freely accessible on the Web: http://webapp.etsi.org/publicationssearch/ http://www.etsi.org/

RE: Disconnect Device for ITE or Lab Equipment Utilizing UPS

1998-10-26 Thread Crabb, John
UL 1778 UPS Equipment requires that a fixed UPS has a disconnect switch for its output (or a cord and plug or receptacle on the output). Otherwise (according to UL 1778) the UPS instruction manual should require that you provide a disconnect device on the UPS output. However, these

RE: Disconnect Device for ITE or Lab Equipment Utilizing UPS

1998-10-26 Thread Crabb, John
within five minutes of activating the remote emergency power off circuit. NEC 645-11, CEC 14-700 John Crabb, Product Safety Engineer, NCR Financial Solutions Group Ltd., Dundee, Scotland. -Original Message- From: CTL [SMTP:c...@prodigy.net] Sent: 26 October 1998 14:11 To: Crabb