RE: swimming pool

2022-02-08 Thread Reed A. Roisum, SET via Sprinklerforum
sprinklers are provided around the perimeter of the pool area. Reed A. Roisum, SET | KFI Engineers | Fire Protection Project Manager | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com -Original Message- From: Sprinklerforum On Behalf Of Bob Caputo via

RE: Dry System Idle Pallets

2021-05-13 Thread Reed A. Roisum, SET via Sprinklerforum
Yes... CMSA... NFPA 13, 2016 ed. Table 12.12.1.2(b) Also, see FMDS 8-24 Table 3... Flow (25) 11.2K uprights at 25 psi I think you could use CMDA criteria from Table A.12.12.1.1(a) and increase the area of operation by 30%?? Reed A. Roisum, SET | KFI Engineers | Fire Protection Project

RE: Interstitial Space

2021-05-11 Thread Reed A. Roisum, SET via Sprinklerforum
that prepare the sprinkler documents have scrutinized areas from which sprinklers can be omitted and limited them to the greatest extent possible. Reed A. Roisum, SET | KFI Engineers | Fire Protection Project Manager | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com

RE: Fire Pump Sprk & Fire Flow Demand

2021-04-21 Thread Reed A. Roisum, SET via Sprinklerforum
Gregg, Take a look at A.11.1.4.2 last paragraph. I don't believe it matters if the water supply for the hydrants is from a fire pump or a municipal supply, the intention is for the sprinkler demand and the fire flow to be separate stand-alone calculations. Reed A. Roisum, SET | KFI

RE: Fire Pump Sprk & Fire Flow Demand

2021-04-21 Thread Reed A. Roisum, SET via Sprinklerforum
and the hose allowance, but not the fire flow. Reed A. Roisum, SET | KFI Engineers | Fire Protection Project Manager | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com -Original Message- From: Sprinklerforum On Behalf Of Gregg Fontes via Sprinklerforum Sent

RE: Question

2020-08-26 Thread Reed A. Roisum, SET via Sprinklerforum
hazard classification in accordance with NFPA 13. Exception: Existing buildings. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> -Original Message-

RE: Pump or Fire Pump

2020-07-08 Thread Reed A. Roisum, SET via Sprinklerforum
to be questioning whether this should be a listed fire pump installed per NFPA 20 or if this is can be looked at as though it is like a municipal system until you hit the backflow. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

Pump or Fire Pump

2020-07-08 Thread Reed A. Roisum, SET via Sprinklerforum
be an acceptable water supply source I couldn’t find a definition of ‘waterworks’ in NFPA or IBC. BTW, 2018 IBC is applicable. Any help or code/standard references are appreciated. Thank you. Reed Roisum Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND

RE: Uprights in non combustible concealed space

2020-06-18 Thread Reed A. Roisum, SET via Sprinklerforum
Ed, I think if you are going to stop posting you should end with a doozy, not something as innocuous as below...stir things up a bit. B-rad ical. Help Mr. Denhardt earn his keep.  Seriously, thank you for all of your wisdom shared. Reed A. Roisum, SET | KFI Engineers | Senior Fire

Under-scoped and under-bid

2020-05-30 Thread Reed A. Roisum, SET via Sprinklerforum
. What will make our industry “push back”? Is there enough of an incentive for sprinkler contractors to “push back”? Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com>

RE: Dust Collection

2020-05-22 Thread Reed A. Roisum, SET via Sprinklerforum
These might also be applicable… NFPA 652: Standard on the Fundamentals of Combustible Dust NFPA 664: Standard for the Prevention of Fires and Explosions in Wood Processing and Woodworking Facilities Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct

RE: Insulation on Valve Risers

2020-04-14 Thread Reed A. Roisum, SET via Sprinklerforum
Check out FMDS 8-29 Refrigerated Storage...particularly the section on 'Prevention of Ice Plugs'. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com>

RE: Curbs for Containment

2020-04-09 Thread Reed A. Roisum, SET via Sprinklerforum
-walled storage tank acts as the secondary means of containment, the exception would allow the omission of the leakage containment area for all flammable and combustible liquids. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile

RE: idle pallets in a 45' building

2020-04-03 Thread Reed A. Roisum, SET via Sprinklerforum
I don't think you will find anything in NFPA 13 higher than 40'. I tried to check FM Global Data Sheet 8-24, but FM's website is down...probably worth taking a look if you have a copy or when the site is back up. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo

RE: [EXTERNAL] RE: Boat and RV storage units

2020-03-19 Thread Reed A. Roisum, SET via Sprinklerforum
-pipe) and 0.5/3000 for ceilings up to 60’. FMDS 3-26 Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum On Behalf Of Fpdcdesign via Sprinkle

RE: [EXTERNAL] Trying to determine hydrant locations per IFC, wondering how sprinkler coverage omissions will affect distances.

2019-10-24 Thread Reed A. Roisum, SET via Sprinklerforum
should be consulted in each case. A building is considered sprinklered throughout when protected in accordance with the requirements of this standard. Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

RE: NFPA 651

2019-10-08 Thread Reed A. Roisum, SET via Sprinklerforum
NFPA 484 Combustible Metals Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum On Behalf Of Easter, Tim (Contractor) via Sprinklerforu

Hotel VTAC Unit "closets"

2019-01-24 Thread Reed A. Roisum, SET
, dryers, furnaces, or water heaters shall be sprinklered, regardless of size. This section is only in New Apartment Buildings and not in New Hotels though. Anyone have a reference that makes it clear whether this space is to be protected or not? Thanks. Reed Roisum Reed A. Roisum, SET | KFI

Hotel VTAC Unit "closets"

2019-01-24 Thread Reed A. Roisum, SET
ment such as washers, dryers, furnaces, or water heaters shall be sprinklered, regardless of size. This section is only in New Apartment Buildings and not in New Hotels though. Anyone have a reference that makes it clear whether this space is to be protected or not? Thanks. Reed Roisum Reed

RE: Back to back floor controls.

2018-11-06 Thread Reed A. Roisum, SET
If you are in NFPA 13, 2013 edition or newer I believe the check valve is required. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinkle

RE: High School Weight Room

2018-10-26 Thread Reed A. Roisum, SET
rooms. Not trying to be difficult Steve, but is having a potential ignition source or not relevant to what the sprinkler density should be? What if you had rack storage of plastics in a room with the only ignition source the house electrical system?? Reed A. Roisum, SET | Karges-Faulconbridge

RE: Exterior Projections

2018-10-12 Thread Reed A. Roisum, SET
ed. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum On Behalf Of John Irwin Sent: Friday, October 12, 2018 5:19 PM To

Fire Pump Acceptance Testing

2018-10-04 Thread Reed A. Roisum, SET
to be performed again? Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: Horizontal Automatic Standpipe Demand

2018-09-07 Thread Reed A. Roisum, SET
State of Minnesota… 2015 MN Building Code Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum On Behalf Of Kyle Montgomer

RE: Horizontal Automatic Standpipe Demand

2018-09-07 Thread Reed A. Roisum, SET
I’m not planning on it…unless the owner requests it. I don’t believe they would be required. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com>

RE: Horizontal Automatic Standpipe Demand

2018-09-05 Thread Reed A. Roisum, SET
No. They didn’t have a requirement for automatic standpipes when the current system was installed as the fire pump is clearly not sized for automatic. We are adding hose connections to meet the building code and replacing the fire pump. Reed A. Roisum, SET | Karges-Faulconbridge, Inc

Horizontal Automatic Standpipe Demand

2018-09-05 Thread Reed A. Roisum, SET
technically only have a single standpipe, I don’t believe we would add another 250 gpm?? Is that correct? I would just flow 250 gpm at the 3 most remote hose connections on third floor?? Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer

Temperature Ratings for Multiple Systems

2018-07-31 Thread Reed A. Roisum, SET
ratings when there are multiple systems that will affect each other if they operate? Or, secondarily, I will take any opinions/justifications on what should be rated what. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND

Paint Booths

2018-07-25 Thread Reed A. Roisum, SET
Materials, which is taken from NFPA 33? EH2, separate valve, cellophane or paper bags over the sprinklers, sprinklers in stacks or ducts spaced every 12', etc. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct

RE: Building Utility Tunnels

2018-05-16 Thread Reed A. Roisum, SET
Not sure about everything in the tunnel, but I know there is some steam piping and domestic water piping. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

Building Utility Tunnels

2018-05-16 Thread Reed A. Roisum, SET
them. I’m not necessarily looking for opinions on whether we should or shouldn’t protect the tunnels, but more so, what the intent of 8.15 is in regards to tunnels or if there are other references in the IBC (2012) or elsewhere that would shed more light. Thank you. Reed Roisum Reed

Concrete Pan Construction

2018-04-27 Thread Reed A. Roisum, SET
13, 2013 ed. 8.6.4.1.2? I believe (1) is the only arrangement that works for this scenario. Was the 1-6” below the bottom of the structural member added in recent years? Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND

Steam Extinguishing Systems

2018-04-16 Thread Reed A. Roisum, SET
nformation… FMDS 06-17 Rotary Kilns and Dryers FMDS 07-10 Wood Processing and Woodworking Facilities FMDS 07-73 Dust Collectors FMDS 07-04 Pulp Dryers Any help or direction is appreciated. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer |

RE: 30% increase for Sloped ceilings

2018-03-27 Thread Reed A. Roisum, SET
It is in 1996. 5-2.3.2.5 Can’t find it in 1989. I don’t have a 1994 or 1991. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinkle

RE: stages

2018-03-15 Thread Reed A. Roisum, SET
s say in accordance with NFPA 13 or 14 and provide sufficient length of hose. So, I take that to mean if you can't cover the stage with the length of hose provided from a single connection, then you would need on both sides. Is that correct Mr. Leyton? Reed A. Roisum, SET | Karges-Faulconbridge

RE: stages

2018-03-15 Thread Reed A. Roisum, SET
Hose connections shall be equipped with an approved adjustable fog nozzle and be mounted in a cabinet or on a rack. I have found that many fire departments do not want these installed so worth checking...actually, State of MN amended out this section in their building code. Reed A. Roisum

RE: Liquor Store

2018-03-15 Thread Reed A. Roisum, SET
Your still kickin' B-rad! Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
think we will be just fine as I suggest. Thank you everyone for the help. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
they are being used. 6.2.1.4 Quick-response sprinklers discharging a minimum of 0.1 gpm/ft2 (4.1 mm/min) shall be permitted to be used in mechanical closets. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
Thanks Travis. Can you please point me to where it says that? Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum

Residential Sprinklers

2018-03-05 Thread Reed A. Roisum, SET
Are residential sprinklers required for dwelling units in NFPA 13R? It appears as though they can be QR or residential in the 2012 IBC (903.3.2). For some reason I had in my mind that they needed to be residential within the dwelling unit or sleeping unit?? Thanks. Reed R. Reed A. Roisum

RE: Underground Dry System Pipe Type

2018-02-19 Thread Reed A. Roisum, SET
Correct. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org

RE: Underground Dry System Pipe Type

2018-02-19 Thread Reed A. Roisum, SET
Thanks Craig. Yes, the valve room is below grade. If we use nitrogen to charge the dry system then would we just use standard DI? Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http

Underground Dry System Pipe Type

2018-02-19 Thread Reed A. Roisum, SET
. Is ductile iron the best option for the underground portion? We are able to slope to drain back to the valve room. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
That’s what I was looking for! Thanks Ben. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforu

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
quantities are taken out and used in the lab facility is there something in NFPA 30 that says protect these areas to OH2? It seems reasonable to me but I need to justify it with something solid and written in the standard. Thanks. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire

RE: Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
It is a medical lab so portions are definitely light hazard but areas that are using and storing the flammable liquids would be OH2 IMO. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

Flammable and Combustible Liquid Storage

2018-02-14 Thread Reed A. Roisum, SET
or combustible liquids are stored in approved cabinets that you basically don't have to account for their presence?...at least I believe that is the intent so please correct me if I am wrong. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer

RE: Nebraska Edition of NFPA 13

2017-12-11 Thread Reed A. Roisum, SET
I do receive Sprinkler Age…didn’t see that I guess. I was able to get an answer from the Assistant Fire Marshal in Omaha. They are in the process of changing to a more current edition, but are currently in the 2002 edition. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire

Nebraska Edition of NFPA 13

2017-12-07 Thread Reed A. Roisum, SET
page is under construction so I am having trouble finding anything definitive. Thank you. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: Barns & Stables

2017-11-06 Thread Reed A. Roisum, SET
for Class III solid pile storage. NFPA 13, 2013 edition 14.2.4 gives design criteria for Class III solid piled over 12 ft in height. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<h

NFPA 13 edition in Wisconsin

2017-10-17 Thread Reed A. Roisum, SET
. It may be because I believe NFPA 1, 2012 edition is the adopted fire code and that would reference NFPA 13, 2010 edition?? Can anyone point me to something definitive for Wisconsin’s applicable edition of NFPA 13? Thank you. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior

"Slatted" Ceiling

2017-10-06 Thread Reed A. Roisum, SET
underneath? Thank you for any insight. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
to take your advice and not pursue any other method of protecting this building besides installing a fire pump and design per the current codes and standards. Thanks for the advice. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND

RE: Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
psi at the elevation of the highest sprinkler in a pipe schedule system, that a fire pump is the only option. Thanks for the thoughts. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

RE: Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
the building, but just wondering if that is the only option, or if there are other, not as good, options. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: Riser Details

2017-10-06 Thread Reed A. Roisum, SET
that would be willing to get you started by walking you through the basics?? 10 minutes and a sketch would go a long ways. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<h

RE: Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongr

RE: Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
Yes. Yes. Yes. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

Pipe Schedule System

2017-10-06 Thread Reed A. Roisum, SET
e schedule and doesn't work hydraulically. Any insight or ideas will be appreciated. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfi

RE: Light Hazaed areas in NFPA 13R Building

2017-08-21 Thread Reed A. Roisum, SET
Good point Steve. One of your most eloquent. :) Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforu

RE: Sprinkler Accessibility

2017-08-15 Thread Reed A. Roisum, SET
Guess I was meaning accessible in the NFPA defined way, “Spaces or concealed areas of construction that can be entered via openable panels, doors hatches, or other readily movable elements (e.g., ceiling tiles).” I’d have to argue the “everything is doable” notion also ☺. Reed A. Roisum, SET

RE: Sprinkler Accessibility

2017-08-15 Thread Reed A. Roisum, SET
another option would be to add gyp to the bottom of the joists and fill above with insulation. Thanks for the input. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<h

Sprinkler Accessibility

2017-08-15 Thread Reed A. Roisum, SET
Do all sprinklers have to be accessible? If so, does anyone have reference? Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

Fire Pump Flowmeter Alternate Means

2017-05-16 Thread Reed A. Roisum, SET
, if it still makes sense to flow water at least every 3 years rather than just use a meter loop. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<h

Fire Pump Test Header Valve Location

2017-05-09 Thread Reed A. Roisum, SET
requires that valve be close to the pump? Thanks. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: FM Global Electrical Room Fire Protection

2017-04-24 Thread Reed A. Roisum, SET
We have consulted the code authority in which I was able to reference the IFC and NFPA 13 standards. We are also going to work with the FM Global Rep but I wanted to have references to the FM Data Sheets if there were any. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire

FM Global Electrical Room Fire Protection

2017-04-22 Thread Reed A. Roisum, SET
to the topic. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

Salvaged Piping

2017-04-11 Thread Reed A. Roisum, SET
piping, not existing. Unfortunately we are using the owner’s spec and not ours so there is more opportunity for shenanigans ☺. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352

RE: Call plates

2017-03-23 Thread Reed A. Roisum, SET
Did you mean calc plates or Hydraulic Design Information Sign? Found in 1996 ed. 8-5 Hydraulic Design Information Sign but can’t see it in 1989 ed. I don’t have anything in between. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct

Cellulose Nitrate Film Storage

2017-03-21 Thread Reed A. Roisum, SET
Does anyone have any experience with Cellulose Nitrate Film storage? NFPA 40 has a lot of good information but I would like to talk with someone with some experience if possible. Thanks. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo

RE: Combined Standpipe/Sprinkler System Floor Controls Location

2017-03-13 Thread Reed A. Roisum, SET
with a listed indicating valve in an accessible location, so located as to control all automatic sources of water supply. 8.16.1.1.7* Control Valve Accessibility. All control valves shall be located where readily accessible and free of obstructions. Reed A. Roisum, SET | Karges-Faulconbridge

Combined Standpipe/Sprinkler System Floor Controls Location

2017-03-13 Thread Reed A. Roisum, SET
, “Permanent ladders, clamped treads on risers, chain-operated hand wheels, or other accepted means should be provided where necessary.” Any guidance is appreciated. Thanks. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct

RE: College Lab Classrooms

2016-12-05 Thread Reed A. Roisum, SET
sense to me that it would depend on the type and quantities of combustible liquids. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinkle

RE: Insert Entryway

2016-10-19 Thread Reed A. Roisum, SET
liquids, or furniture. Incidental combustible storage in the vestibule is limited to 5 ft3 of material. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.

RE: Question for any member of Installation Sub-TC

2016-09-27 Thread Reed A. Roisum, SET
Does “log-grade” mean worse than finished lumber grade? Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforu

RE: Apparatus Bays

2016-08-22 Thread Reed A. Roisum, SET
, the potential for a shielded fire. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforu

RE: Sprinkler Zones in Multi-Tenant Building (Roland Huggins)

2016-08-15 Thread Reed A. Roisum, SET
Thanks Rick. No, the supply piping to each tenant is above ground. The controls for the building are located near the center of the building and supplied with overhead piping from there. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct

RE: Sprinkler Zones in Multi-Tenant Building

2016-08-10 Thread Reed A. Roisum, SET
Mississauga. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

Sprinkler Zones in Multi-Tenant Building

2016-08-10 Thread Reed A. Roisum, SET
. Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfiengineers.com> __ This ema

Stage Calc Hose Allowance

2016-08-02 Thread Reed A. Roisum, SET
tem design at that point. [cid:image002.png@01D1ECA8.ED095E10] Thank you. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | KFIengineers.com<http://www.kfi

FM Global Design Area

2016-06-27 Thread Reed A. Roisum, SET
find if that is to flow 4 sprinklers on 3 lines or 3 sprinklers on 4 lines or something else?? Can anyone point me to where you determine how many sprinklers per line to include? Thanks. Reed Roisum Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND

RE: Hose Valves for Stage

2016-05-06 Thread Reed A. Roisum, SET
and be mounted in a cabinet or on a rack. If you choose to install a 1 1/2" hose connection in accordance with NFPA 13, go to 8.17.5 (2013 ed.). Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |

RE: High-Speed and Ultra-High Speed Deluge Systems

2016-03-24 Thread Reed A. Roisum, SET
Chris, Have you looked at Pyrotech? http://pyrotechusa.com/ What is the application? Explosion protection? Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com

RE: ESFR & Smoke Vents

2016-03-24 Thread Reed A. Roisum, SET
oordinated with the sprinkler operating temperatures. NFPA 13, 2013 ed. 12.1.1.2 "ESFR sprinklers shall not be used in buildings with automatic heat or smoke vents unless the vents use a high-temperature rated, standard-response operating mechanism." Reed A. Roisum, SET | Karge

RE: PVC FOR INCOMING SERVICE SUPPLY

2016-03-24 Thread Reed A. Roisum, SET
s a 'private fire service main' is that pipe between a source of water and the water supply side of the first above ground connection to a sprinkler or standpipe system. Thanks. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903

RE: Room Design and Unprotected Pockets

2016-01-25 Thread Reed A. Roisum, SET
sayin'... :) Sincerely, Les B. Consistent Deputy of Grammar and Spelling Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum

RE: individual garages for apt buildings - NFPA 13

2016-01-15 Thread Reed A. Roisum, SET
You just have to remember that if you are in a burning car you should get out before you enter the garage...or, make sure you shut the garage door once inside. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile

RE: Fire Flow vs Hydraulic calc's

2015-12-22 Thread Reed A. Roisum, SET
IFC 2012, Appendix B Section B105 Fire-Flow Requirements For Buildings Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum

RE: Clean room sprinklers

2015-08-28 Thread Reed A. Roisum, SET
-combustible construction but the plastic sheeting for walls is going to be a hurdle I would guess. Thanks. Reed Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com

RE: Standpipes

2015-04-22 Thread Reed A. Roisum, SET
of the highest story is located more than 30 feet above the lowest level of the FD vehicle access. Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From

RE: Standpipes

2015-04-22 Thread Reed A. Roisum, SET
? Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve

RE: Standpipes

2015-04-22 Thread Reed A. Roisum, SET
Steve agrees that the IFC commentary figure does not agree with the code language and should be disregarded. A mezzanine is clearly not a story. Sorry for the confusion...I thought I was safe when I was just quoting what I read in the code commentary. Reed A. Roisum, SET | Karges